43-CFD Configuration Examples
Title Size Download
43-CFD Configuration Examples 175.67 KB

 

H3C S6805&S6825&S6850 & S9850 & S9820

CFD Configuration Examples

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

Copyright © 2020-2023 New H3C Technologies Co., Ltd. All rights reserved.

No part of this manual may be reproduced or transmitted in any form or by any means without prior written consent of New H3C Technologies Co., Ltd.

Except for the trademarks of New H3C Technologies Co., Ltd., any trademarks that may be mentioned in this document are the property of their respective owners.

The information in this document is subject to change without notice.

 



Introduction

This document provides CFD configuration examples.

CFD is used for link connectivity detection, fault verification, and fault location in Layer 2 networks.

Prerequisites

The configuration examples in this document were created and verified in a lab environment, and all the devices were started with the factory default configuration. When you are working on a live network, make sure you understand the potential impact of every command on your network.

This document assumes that you have basic knowledge of CFD.

Example: Configuring CFD

Network configuration

As shown in Figure 1, Device B and Device C reside in the central equipment room of a company. Device A, Device D, and Device E reside in other areas.

·     Research and development department users in VLAN 20 access the enterprise network through Device A and Device D.

·     Marketing department users in VLAN 30 access the enterprise network through Device A and Device E.

Configure CFD to verify and locate link faults.

Figure 1 Network diagram

 

Analysis

To accurately locate link faults, assign the enterprise network to MD_A (level 5) and the central equipment room network to MD_B (level 3). MD_A nests MD_B.

To effectively implement CFD, assign MAs based on the VLANs of service traffic:

·     Assign VLAN 20 in MD_A to MA_A_1.

·     Assign VLAN 30 in MD_A to MA_A_2.

·     Assign VLAN 20 in MD_B to MA_B_1.

·     Assign VLAN 30 in MD_B to MA_A_2.

To verify link connectivity, configure MEPs on the interfaces located at the boundary of MAs, for example, MA_B_1:

·     Configure MEPs on interface HGE1/0/1 of Device B and Device D to allow CFD packets from VLAN 20 to pass through the following interfaces:

¡     HGE1/0/1 and HGE1/0/2 of Device B.

¡     HGE1/0/1 and HGE1/0/2 of Device C.

¡     HGE1/0/1 of Device D.

·     Configure HGE1/0/1 of Device B as an inward-facing MEP because CFD packets are forwarded through other interfaces on the device.

·     Configure HGE1/0/1 of Device D as an outward-facing MEP because CFD packets are forwarded through the interface.

To accurately locate link faults between Device B and Device D, configure the default MIP generation rule on Device C.

To detect connectivity among MEPs, configure CC on the MEPs.

To verify link faults detected through CC, use LB. To trace faulty paths or locate link faults, use LT after the status information of the entire network is obtained.

Figure 2 shows a CFD configuration diagram based on the previous analysis.

Figure 2 CFD configuration diagram

 

Applicable hardware and software versions

The following matrix shows the hardware and software versions to which this configuration example is applicable:

 

Hardware

Software version

S6805 switch series

Release 6607, Release 6616, Release 6616P01, Release 6635 and later

S6825 switch series

Release 6616, Release 6616P01, Release 6635 and later

S6850 switch series

S9850 switch series

Release 6555P01, Release 6607, Release 6616, Release 6616P01, Release 6635 and later

S9820-64H switch

Release 6555P01, Release 6607, Release 6616, Release 6616P01, Release 6635 and later

S9820-8C switch

Release 6607, Release 6616, Release 6616P01, Release 6635 and later

 

Restrictions and guidelines

When you configure CFD, follow these restrictions and guidelines:

·     You cannot create a MEP if the MEP ID is not included in the MEP list of the service instance.

·     You can configure multiple MAs in an MD as needed. An MA serves only one VLAN.

·     Configure the same CCM interval field value for all MEPs in the same MA. In this example, the MEPs use the default CCM interval field value.

Procedures

Enabling CFD

# Enable CFD on Device A.

<DeviceA> system-view

[DeviceA] cfd enable

# Enable CFD on Device B through Device E. (Details not shown.)

Creating VLANs and assigning interfaces to the VLANs

1.     Configure Device A:

[DeviceA] vlan 20

[DeviceA-vlan20] quit

[DeviceA] vlan 30

[DeviceA-vlan30] quit

[DeviceA] interface hundredgige 1/0/1

[DeviceA-HundredGigE1/0/1] port access vlan 20

[DeviceA-HundredGigE1/0/1] quit

[DeviceA] interface hundredgige 1/0/2

[DeviceA-HundredGigE1/0/2] port access vlan 30

[DeviceA-HundredGigE1/0/2] quit

[DeviceA] interface hundredgige 1/0/3

[DeviceA-HundredGigE1/0/3] port link-type trunk

[DeviceA-HundredGigE1/0/3] port trunk permit vlan 20 30

[DeviceA-HundredGigE1/0/3] quit

2.     Configure Device B:

[DeviceB] vlan 20

[DeviceB-vlan20] quit

[DeviceB] vlan 30

[DeviceB-vlan30] quit

[DeviceB] interface hundredgige 1/0/1

[DeviceB-HundredGigE1/0/1] port link-type trunk

[DeviceB-HundredGigE1/0/1] port trunk permit vlan 20 30

[DeviceB-HundredGigE1/0/1] quit

[DeviceB] interface hundredgige 1/0/2

[DeviceB-HundredGigE1/0/2] port link-type trunk

[DeviceB-HundredGigE1/0/2] port trunk permit vlan 20

[DeviceB-HundredGigE1/0/2] quit

[DeviceB] interface hundredgige 1/0/3

[DeviceB-HundredGigE1/0/3] port link-type trunk

[DeviceB-HundredGigE1/0/3] port trunk permit vlan 30

[DeviceB-HundredGigE1/0/3] quit

3.     Configure Device C:

[DeviceC] vlan 20

[DeviceC-vlan20] quit

[DeviceC] interface hundredgige 1/0/1

[DeviceC-HundredGigE1/0/1] port link-type trunk

[DeviceC-HundredGigE1/0/1] port trunk permit vlan 20

[DeviceC-HundredGigE1/0/1] quit

[DeviceC] interface hundredgige 1/0/2

[DeviceC-HundredGigE1/0/2] port link-type trunk

[DeviceC-HundredGigE1/0/2] port trunk permit vlan 20

[DeviceC-HundredGigE1/0/2] quit

4.     Configure Device D:

[DeviceD] vlan 20

[DeviceD-vlan20] quit

[DeviceD] interface hundredgige 1/0/1

[DeviceD-HundredGigE1/0/1] port link-type trunk

[DeviceD-HundredGigE1/0/1] port trunk permit vlan 20

[DeviceD-HundredGigE1/0/1] quit

[DeviceD] interface hundredgige 1/0/2

[DeviceD-HundredGigE1/0/2] port access vlan 20

[DeviceD-HundredGigE1/0/2] quit

5.     Configure Device E:

[DeviceE] vlan 30

[DeviceE-vlan30] quit

[DeviceE] interface hundredgige 1/0/1

[DeviceE-HundredGigE1/0/1] port access vlan 30

[DeviceE-HundredGigE1/0/1] quit

[DeviceE] interface hundredgige 1/0/2

[DeviceE-HundredGigE1/0/2] port link-type trunk

[DeviceE-HundredGigE1/0/2] port trunk permit vlan 30

[DeviceE-HundredGigE1/0/2] quit

Configuring service instances

Based on the MAs to which the MEPs belong, perform the configurations as described in the following table:

 

Device

MD

MD level

MA

VLAN

Service instance

Device A

MD_A

5

MA_A_1

20

1

MA_A_2

30

2

Device B

MD_B

3

MA_B_1

20

3

MA_B_2

30

4

Device C

MD_B

3

MA_B_1

20

3

Device D

MD_A

5

MA_A_1

20

1

MD_B

3

MA_B_1

20

3

Device E

MD_A

5

MA_A_2

30

2

MD_B

3

MA_B_2

30

4

 

1.     Configure Device A:

# Create MD_A (level 5).

[DeviceA] cfd md MD_A level 5

# Create service instance 1, in which the MA named MA_A_1 serves VLAN 20.

[DeviceA] cfd service-instance 1 ma-id string MA_A_1 md MD_A vlan 20

# Create service instance 2, in which the MA named MA_A_2 serves VLAN 30.

[DeviceA] cfd service-instance 2 ma-id string MA_A_2 md MD_A vlan 30

Configure Device B through Device E in the same way Device A is configured.

2.     Configure Device B:

[DeviceB] cfd md MD_B level 3

[DeviceB] cfd service-instance 3 ma-id string MA_B_1 md MD_B vlan 20

[DeviceB] cfd service-instance 4 ma-id string MA_B_2 md MD_B vlan 30

3.     Configure Device C:

[DeviceC] cfd md MD_B level 3

[DeviceC] cfd service-instance 3 ma-id string MA_B_1 md MD_B vlan 20

4.     Configure Device D:

[DeviceD] cfd md MD_A level 5

[DeviceD] cfd service-instance 1 ma-id string MA_A_1 md MD_A vlan 20

[DeviceD] cfd md MD_B level 3

[DeviceD] cfd service-instance 3 ma-id string MA_B_1 md MD_B vlan 20

5.     Configure Device E:

[DeviceE] cfd md MD_A level 5

[DeviceE] cfd service-instance 2 ma-id string MA_A_2 md MD_A vlan 30

[DeviceE] cfd md MD_B level 3

[DeviceE] cfd service-instance 4 ma-id string MA_B_2 md MD_B vlan 30

Configuring MEPs

Assign MEP IDs as described in the following table:

 

Service instance

Device

Interface

MEP ID

MEP type

1

Device A

HundredGigE 1/0/1

1001

Inward-facing MEP

Device D

HundredGigE 1/0/2

1002

Inward-facing MEP

2

Device A

HundredGigE 1/0/2

2001

Inward-facing MEP

Device E

HundredGigE 1/0/1

2002

Inward-facing MEP

3

Device B

HundredGigE 1/0/1

3001

Inward-facing MEP

Device D

HundredGigE 1/0/1

3002

Outward-facing MEP

4

Device B

HundredGigE 1/0/1

4001

Inward-facing MEP

Device E

HundredGigE 1/0/2

4002

Outward-facing MEP

 

1.     Configure Device A:

# Configure a MEP list in service instances 1 and 2.

[DeviceA] cfd meplist 1001 1002 service-instance 1

[DeviceA] cfd meplist 2001 2002 service-instance 2

# Create inward-facing MEP 1001 in service instance 1 on HundredGigE 1/0/1.

[DeviceA] interface hundredgige 1/0/1

[DeviceA-HundredGigE1/0/1] cfd mep 1001 service-instance 1 inbound

[DeviceA-HundredGigE1/0/1] quit

# Create inward-facing MEP 2001 in service instance 2 on HundredGigE 1/0/2.

[DeviceA] interface hundredgige 1/0/2

[DeviceA-HundredGigE1/0/2] cfd mep 2001 service-instance 2 inbound

[DeviceA-HundredGigE1/0/2] quit

Configure Device B, Device D, and Device E in the same way Device A is configured.

2.     Configure Device B:

[DeviceB] cfd meplist 3001 3002 service-instance 3

[DeviceB] cfd meplist 4001 4002 service-instance 4

[DeviceB] interface hundredgige 1/0/1

[DeviceB-HundredGigE1/0/1] cfd mep 3001 service-instance 3 inbound

[DeviceB-HundredGigE1/0/1] cfd mep 4001 service-instance 4 inbound

[DeviceB-HundredGigE1/0/1] quit

3.     Configure Device D:

[DeviceD] cfd meplist 1001 1002 service-instance 1

[DeviceD] cfd meplist 3001 3002 service-instance 3

[DeviceD] interface hundredgige 1/0/2

[DeviceD-HundredGigE1/0/2] cfd mep 1002 service-instance 1 inbound

[DeviceD-HundredGigE1/0/2] quit

[DeviceD] interface hundredgige 1/0/1

[DeviceD-HundredGigE1/0/1] cfd mep 3002 service-instance 3 outbound

[DeviceD-HundredGigE1/0/1] quit

4.     Configure Device E:

[DeviceE] cfd meplist 2001 2002 service-instance 2

[DeviceE] cfd meplist 4001 4002 service-instance 4

[DeviceE] interface hundredgige 1/0/1

[DeviceE-HundredGigE1/0/1] cfd mep 2002 service-instance 2 inbound

[DeviceE-HundredGigE1/0/1] quit

[DeviceE] interface hundredgige 1/0/2

[DeviceE-HundredGigE1/0/2] cfd mep 4002 service-instance 4 outbound

[DeviceE-HundredGigE1/0/2] quit

Configuring a MIP generation rule

# Configure the MIP generation rule in service instance 3 on Device C as default.

[DeviceC] cfd mip-rule default service-instance 3

Configuring CC on MEPs

1.     Configure Device A:

# Enable the sending of CCM frames for MEP 1001 in service instance 1 on HundredGigE 1/0/1.

[DeviceA] interface hundredgige 1/0/1

[DeviceA-HundredGigE1/0/1] cfd cc service-instance 1 mep 1001 enable

[DeviceA-HundredGigE1/0/1] quit

# Enable the sending of CCM frames for MEP 2001 in service instance 2 on HundredGigE 1/0/2.

[DeviceA] interface hundredgige 1/0/2

[DeviceA-HundredGigE1/0/2] cfd cc service-instance 2 mep 2001 enable

[DeviceA-HundredGigE1/0/2] quit

Configure Device B, Device D, and Device E in the same way Device A is configured.

2.     Configure Device B:

[DeviceB] interface hundredgige 1/0/1

[DeviceB-HundredGigE1/0/1] cfd cc service-instance 3 mep 3001 enable

[DeviceB-HundredGigE1/0/1] cfd cc service-instance 4 mep 4001 enable

[DeviceB-HundredGigE1/0/1] quit

3.     Configure Device D:

[DeviceD] interface hundredgige 1/0/1

[DeviceD-HundredGigE1/0/1] cfd cc service-instance 3 mep 3002 enable

[DeviceD-HundredGigE1/0/1] quit

[DeviceD] interface hundredgige 1/0/2

[DeviceD-HundredGigE1/0/2] cfd cc service-instance 1 mep 1002 enable

[DeviceD-HundredGigE1/0/2] quit

4.     Configure Device E:

[DeviceE] interface hundredgige 1/0/1

[DeviceE-HundredGigE1/0/1] cfd cc service-instance 2 mep 2002 enable

[DeviceE-HundredGigE1/0/1] quit

[DeviceE] interface hundredgige 1/0/2

[DeviceE-HundredGigE1/0/2] cfd cc service-instance 4 mep 4002 enable

[DeviceE-HundredGigE1/0/2] quit

Verifying the configuration

In this example, the MAC addresses of Device A through Device E are 0010-FC01-6511, 0010-FC02-6512, 0010-FC03-6513, 0010-FC04-6514, and 0010-FC05-6515, respectively.

1.     Verify the configuration when the network is operating correctly:

# Display information about remote MEP 1001 in service instance 1 on Device A.

[DeviceA] display cfd remote-mep service-instance 1 mep 1001

MEP ID   MAC address      State        Time                  MAC status

1002     0010-fc04-6514   OK           2019/07/26 12:54:52   UP

The output shows that the remote MEP is operating correctly.

# Enable LB on Device A to verify the status of the link between MEP 1001 and MEP 1002 in service instance 1.

[DeviceA] cfd loopback service-instance 1 mep 1001 target-mep 1002

Loopback to MEP 1002 with the sequence number start from 1001-43404:

Reply from 0010-fc04-6514: sequence number=1001-43404 Time=5ms

Reply from 0010-fc04-6514: sequence number=1001-43405 Time=5ms

Reply from 0010-fc04-6514: sequence number=1001-43406 Time=5ms

Reply from 0010-fc04-6514: sequence number=1001-43407 Time=5ms

Reply from 0010-fc04-6514: sequence number=1001-43408 Time=5ms

Sent: 5        Received: 5        Lost: 0

The output shows that no link fault occurs on the link between MEP 1001 and MEP 1002 in service instance 1.

2.     Verify the configuration when a link fault occurs:

# Display information about remote MEP 1001 in service instance 1 on Device A.

[DeviceA] display cfd remote-mep service-instance 1 mep 1001

MEP ID   MAC address      State        Time                  MAC status

1002     0010-fc04-6514   FAILED       2019/07/26 13:01:52   DOWN

The output shows that the remote MEP is operating incorrectly.

# Enable LB on Device A to verify the status of the link between MEP 1001 and MEP 1002 in service instance 1.

[DeviceA] cfd loopback service-instance 1 mep 1001 target-mep 1002

Loopback to MEP 1002 with the sequence number start from 1001-43904:

Sent: 5        Received: 0        Lost: 5

The output shows that a link fault occurs on the link between MEP 1001 and MEP 1002 in service instance 1.

# Identify the path between MEP 3001 and MEP 3002 in service instance 3 on Device B.

[DeviceB] cfd linktrace service-instance 3 mep 3001 target-mep 3002

Linktrace to MEP 3002 with the sequence number 3001-43862:

MAC Address               TTL     Last Mac         Relay Action

0010-fc03-6513            63      0010-fc02-6512   MPDB

The output shows that MEP 3001 receives only the LTR messages from the MIP. No LTR messages are sent from MEP 3002 (HundredGigE 1/0/1 on Device D). The link between Device C and Device D fails, and you do not need to troubleshoot the network outside MD_B.

Configuration files

·     Device A:

#

 cfd enable

 cfd md MD_A index 1 level 5

 cfd service-instance 1 ma-id string MA_A_1 ma-index 1 md MD_A vlan 20

 cfd meplist 1001 to 1002 service-instance 1

 cfd service-instance 2 ma-id string MA_A_2 ma-index 1 md MD_A vlan 30

 cfd meplist 2001 to 2002 service-instance 2

#

vlan 20

#

vlan 30

#

interface HundredGigE1/0/1

 port link-mode bridge

 port access vlan 20

 cfd mep 1001 service-instance 1 inbound

 cfd cc service-instance 1 mep 1001 enable

#

interface HundredGigE1/0/2

 port link-mode bridge

 port access vlan 30

 cfd mep 2001 service-instance 2 inbound

 cfd cc service-instance 2 mep 2001 enable

#

interface HundredGigE1/0/3

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 20 30

·     Device B:

#

 cfd enable

 cfd md MD_B index 1 level 3

 cfd service-instance 3 ma-id string MA_B_1 ma-index 1 md MD_B vlan 20

 cfd meplist 3001 to 3002 service-instance 3

 cfd service-instance 4 ma-id string MA_B_2 ma-index 2 md MD_B vlan 30

 cfd meplist 4001 to 4002 service-instance 4

#

vlan 20

#

vlan 30

#

interface HundredGigE1/0/1

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 20 30

 cfd mep 3001 service-instance 3 inbound

 cfd cc service-instance 3 mep 3001 enable

 cfd mep 4001 service-instance 4 inbound

 cfd cc service-instance 4 mep 4001 enable

#

interface HundredGigE1/0/2

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 20

#

interface HundredGigE1/0/3

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 30

·     Device C:

#

 cfd enable

 cfd md MD_B index 1 level 3

 cfd service-instance 3 ma-id string MA_B_1 ma-index 1 md MD_B vlan 20

 cfd mip-rule default service-instance 3

#

vlan 20

#

interface HundredGigE1/0/1

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 20

#

interface HundredGigE1/0/2

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 20

·     Device D:

#

 cfd enable

 cfd md MD_A index 1 level 5

 cfd md MD_B index 2 level 3

 cfd service-instance 1 ma-id string MA_A_1 ma-index 1 md MD_A vlan 20

 cfd meplist 1001 to 1002 service-instance 1

 cfd service-instance 3 ma-id string MA_B_1 ma-index 1 md MD_B vlan 20

 cfd meplist 3001 to 3002 service-instance 3

#

vlan 20

#

interface HundredGigE1/0/1

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 20

 cfd mep 3002 service-instance 3 outbound

 cfd cc service-instance 3 mep 3002 enable

#

interface HundredGigE1/0/2

 port link-mode bridge

 port access vlan 20

 cfd mep 1002 service-instance 1 inbound

 cfd cc service-instance 1 mep 1002 enable

·     Device E:

#

 cfd enable

 cfd md MD_A index 1 level 5

 cfd md MD_B index 2 level 3

 cfd service-instance 2 ma-id string MA_A_2 ma-index 1 md MD_A vlan 30

 cfd meplist 2001 to 2002 service-instance 2

 cfd service-instance 4 ma-id string MA_B_2 ma-index 2 md MD_B vlan 30

 cfd meplist 4001 to 4002 service-instance 4

#

vlan 30

#

interface HundredGigE1/0/1

 port link-mode bridge

 port access vlan 30

 cfd mep 2002 service-instance 2 inbound

 cfd cc service-instance 2 mep 2002 enable

#

interface HundredGigE1/0/2

 port link-mode bridge

 port link-type trunk

 port trunk permit vlan 30

 cfd mep 4002 service-instance 4 outbound

 cfd cc service-instance 4 mep 4002 enable

Related documentation

Use this document in conjunction with the following documents for the product and software version you are working with:

·     High Availability Command Reference

·     High Availability Configuration Guide

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
All Support
  • Become a Partner
  • Partner Resources
  • Partner Business Management
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us
新华三官网