Configuring loop detection

About loop detection

The loop detection mechanism performs periodic checking for Layer 2 loops. The mechanism immediately generates a log when a loop occurs so that you are promptly notified to adjust network connections and configurations. You can configure loop detection to shut down the looped interface. Logs are maintained in the information center. For more information, see Network Management and Monitoring Configuration Guide.

Loop detection mechanism

The device detects loops by sending detection frames and then checking whether these frames return to any interface on the device. If they do, the device considers that the interface is on a looped link.

Loop detection usually works within a VLAN. If a detection frame is returned with a different VLAN tag than it was sent out with, an inter-VLAN loop has occurred. To remove the loop, examine the QinQ or VLAN mapping configuration for incorrect settings. For more information about QinQ and VLAN mapping, see "Configuring QinQ" and "Configuring VLAN mapping."

Figure 1 Ethernet frame header for loop detection

The Ethernet frame header of a loop detection packet contains the following fields:

·     DMACDestination MAC address of the frame, which is the multicast MAC address 010f-e200-0007. When a loop detection-enabled device receives a frame with this destination MAC address, it performs the following operations:

¡     Sends the frame to the CPU.

¡     Floods the frame in the VLAN from which the frame was originally received.

·     SMACSource MAC address of the frame, which is the bridge MAC address of the sending device.

·     TPIDType of the VLAN tag, with the value of 0x8100.

·     TCIInformation of the VLAN tag, including the priority and VLAN ID.

·     TypeProtocol type, with the value of 0x8918.

Figure 2 Inner frame header for loop detection

The inner frame header of a loop detection packet contains the following fields:

·     CodeProtocol sub-type, which is 0x0001, indicating the loop detection protocol.

·     VersionProtocol version, which is always 0x0000.

·     LengthLength of the frame. The value includes the inner header, but excludes the Ethernet header.

·     ReservedThis field is reserved.

Frames for loop detection are encapsulated as TLV triplets.

Table 1 TLVs supported by loop detection

TLV

Description

Remarks

End of PDU

End of a PDU.

Optional.

Device ID

Bridge MAC address of the sending device.

Required.

Port ID

ID of the PDU sending interface.

Optional.

Port Name

Name of the PDU sending interface.

Optional.

System Name

Device name.

Optional.

Chassis ID

Chassis ID of the sending interface.

Optional.

Slot ID

Slot ID of the sending interface.

Optional.

Sub Slot ID

Sub-slot ID of the sending interface.

Optional.

Loop detection interval

Loop detection is a continuous process as the network changes. Loop detection frames are sent at the loop detection interval to determine whether loops occur on interfaces and whether loops are removed.

Loop protection actions

When the device detects a loop on an interface, it generates a log but performs no action on the interface by default. You can configure the device to take one of the following actions:

·     Block—Disables the interface from learning MAC addresses and blocks the interface.

·     No-learning—Disables the interface from learning MAC addresses.

·     Shutdown—Shuts down the interface to disable it from receiving and sending any frames.

Loop protection delay

The loop protection delay enables the device to wait for a period of time before taking loop protection actions on looped interfaces. On a network protected by loop detection, the shutdown or block action taken on a looped interface of an upstream device might cause traffic interruption to its downstream devices. To minimize the impacts of loop detection on downstream traffic, set the loop protection delay on the upstream devices. This delay allows the downstream devices to remove loops before the upstream devices take an action.

Interface status auto recovery

When the device configured with the block or no-learning loop action detects a loop on an interface, it performs the action and waits three loop detection intervals. If the device does not receive a loop detection frame within three loop detection intervals, it performs the following operations:

·     Automatically sets the interface to the forwarding state.

·     Notifies the user of the event.

When the device configured with the shutdown action detects a loop on an interface, the following events occur:

1.     The device automatically shuts down the interface.

2.     The device automatically sets the interface to the forwarding state after the detection timer set by using the shutdown-interval command expires. For more information about the shutdown-interval command, see Fundamentals Command Reference.

3.     The device shuts down the interface again if a loop is still detected on the interface when the detection timer expires.

This process is repeated until the loop is removed.

 

 

NOTE:

Incorrect recovery can occur when loop detection frames are discarded to reduce the load. To avoid this, use the shutdown action, or manually remove the loop.

Restriction and guidelines: DRNI configuration

Member devices in a M-LAG system must have the same loop detection configuration.

Loop detection tasks at a glance

To configure loop detection, perform the following tasks:

1.     Enabling loop detection

¡     Enabling loop detection globally

¡     Enabling loop detection on an interface

2.     (Optional) Setting the loop protection action

¡     Setting the global loop protection action

¡     Setting the loop protection action on an interface

3.     (Optional) Setting the loop detection interval

4.     (Optional) Setting the loop protection delay timer

¡     Setting the global loop protection delay timer

¡     Setting the loop protection delay timer on an interface

Enabling loop detection

Restrictions and guidelines for loop detection configuration

You can enable loop detection globally or on a per-interface basis. When an interface receives a detection frame in any VLAN, the loop protection action is triggered on that interface, regardless of whether loop detection is enabled on it.

If you have enabled loop detection globally, do not set the loop protection action to block when you configure loop detection on a per-interface basis.

Enabling loop detection globally

1.     Enter system view.

system-view

2.     Globally enable loop detection.

loopback-detection global enable vlan { vlan-id--list | all }

By default, loop detection is globally disabled.

Enabling loop detection on an interface

1.     Enter system view.

system-view

2.     Enter Layer 2 Ethernet interface view or Layer 2 aggregate interface view.

interface interface-type interface-number

3.     Enable loop detection on the interface.

loopback-detection enable vlan { vlan-id--list | all }

By default, loop detection is disabled on interfaces.

Setting the loop protection action

Restrictions and guidelines for loop protection action configuration

You can set the loop protection action globally or on a per-interface basis. The global action applies to all interfaces. An interface-specific action applies to the interface on which it is configured. On an interface, the interface-specific action takes precedence over the global action.

Setting the global loop protection action

1.     Enter system view.

system-view

2.     Set the global loop protection action.

loopback-detection global action shutdown

By default, the device generates a log but performs no action on the interface on which a loop is detected.

Setting the loop protection action on an interface

1.     Enter system view.

system-view

2.     Enter interface view.

interface interface-type interface-number

3.     Set the loop protection action on the interface.

loopback-detection action { block | no-learning | shutdown }

By default, the device generates a log but performs no action on the interface on which a loop is detected.

Support for the keywords of this command varies by interface type. For more information, see Layer 2LAN Switching Command Reference.

Setting the loop detection interval

About this task

With loop detection enabled, the device sends loop detection frames at the loop detection interval. A shorter interval offers more sensitive detection but consumes more resources. Consider the system performance and loop detection speed when you set the loop detection interval.

Procedure

1.     Enter system view.

system-view

2.     Set the loop detection interval.

loopback-detection interval-time interval

The default setting is 30 seconds.

Setting the loop protection delay timer

Restrictions and guidelines for loop protection delay timer configuration

The global delay timer applies to all interfaces enabled with loop detection. An interface-specific delay timer applies to the interface on which it is configured. On an interface, the interface-specific delay timer takes precedence over the global delay timer.

To prevent interfaces from going down or coming up concurrently, set the loop protection delay timer to different values on different devices or on different interfaces of the same device.

Setting the global loop protection delay timer

1.     Enter system view.

system-view

2.     Set the global loop protection delay timer.

loopback-detection global delay-timer time

By default, loop protection delay is disabled globally.

Setting the loop protection delay timer on an interface

1.     Enter system view.

system-view

2.     Enter interface view.

interface interface-type interface-number

3.     Set the loop protection delay timer on the interface.

loopback-detection global delay-timer time

By default, loop protection delay is disabled on an interface.

Display and maintenance commands for loop detection

Execute display commands in any view.

 

Task

Command

Display the loop detection configuration and status.

display loopback-detection

Loop detection configuration examples

Example: Configuring basic loop detection functions

Network configuration

As shown in Figure 3, configure loop detection on Device A to meet the following requirements:

·     Device A generates a log as a notification.

·     Device A automatically shuts down the interface on which a loop is detected.

Figure 3 Network diagram

 

Procedure

1.     Configure Device A:

# Create VLAN 100, and globally enable loop detection for the VLAN.

<DeviceA> system-view

[DeviceA] vlan 100

[DeviceA-vlan100] quit

[DeviceA] loopback-detection global enable vlan 100

# Configure Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 as trunk ports, and assign them to VLAN 100.

[DeviceA] interface Ten-GigabitEthernet 3/0/1

[DeviceA-Ten-GigabitEthernet3/0/1] port link-type trunk

[DeviceA-Ten-GigabitEthernet3/0/1] port trunk permit vlan 100

[DeviceA-Ten-GigabitEthernet3/0/1] quit

[DeviceA] interface ten-gigabitethernet 3/0/2

[DeviceA-Ten-GigabitEthernet3/0/2] port link-type trunk

[DeviceA-Ten-GigabitEthernet3/0/2] port trunk permit vlan 100

[DeviceA-Ten-GigabitEthernet3/0/2] quit

# Set the global loop protection action to shutdown.

[DeviceA] loopback-detection global action shutdown

# Set the loop detection interval to 35 seconds.

[DeviceA] loopback-detection interval-time 35

2.     Configure Device B:

# Create VLAN 100.

<DeviceB> system-view

[DeviceB] vlan 100

[DeviceB–vlan100] quit

# Configure Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 as trunk ports, and assign them to VLAN 100.

[DeviceB] interface ten-gigabitethernet 3/0/1

[DeviceB-Ten-GigabitEthernet3/0/1] port link-type trunk

[DeviceB-Ten-GigabitEthernet3/0/1] port trunk permit vlan 100

[DeviceB-Ten-GigabitEthernet3/0/1] quit

[DeviceB] interface ten-gigabitethernet 3/0/2

[DeviceB-Ten-GigabitEthernet3/0/2] port link-type trunk

[DeviceB-Ten-GigabitEthernet3/0/2] port trunk permit vlan 100

[DeviceB-Ten-GigabitEthernet3/0/2] quit

3.     Configure Device C:

# Create VLAN 100.

<DeviceC> system-view

[DeviceC] vlan 100

[DeviceC–vlan100] quit

# Configure Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 as trunk ports, and assign them to VLAN 100.

[DeviceC] interface ten-gigabitethernet 3/0/1

[DeviceC-Ten-GigabitEthernet3/0/1] port link-type trunk

[DeviceC-Ten-GigabitEthernet3/0/1] port trunk permit vlan 100

[DeviceC-Ten-GigabitEthernet3/0/1] quit

[DeviceC] interface ten-gigabitethernet 3/0/2

[DeviceC-Ten-GigabitEthernet3/0/2] port link-type trunk

[DeviceC-Ten-GigabitEthernet3/0/2] port trunk permit vlan 100

[DeviceC-Ten-GigabitEthernet3/0/2] quit

Verifying the configuration

# View the system logs on devices, for example, Device A.

[DeviceA]

%Feb 24 15:04:29:663 2019 DeviceA LPDT/4/LPDT_LOOPED:  A loop was detected on Ten-GigabitEthernet3/0/1.

%Feb 24 15:04:29:664 2019 DeviceA LPDT/4/LPDT_VLAN_LOOPED: A loop was detected on Ten-GigabitEthernet3/0/1 in VLAN 100.

%Feb 24 15:04:29:667 2019 DeviceA LPDT/4/LPDT_LOOPED: A loop was detected on Ten-GigabitEthernet3/0/2.

%Feb 24 15:04:29:668 2019 DeviceA LPDT/4/LPDT_VLAN_LOOPED: A loop was detected on Ten-GigabitEthernet3/0/2 in VLAN 100.

%Feb 24 15:04:44:243 2019 DeviceA LPDT/5/LPDT_VLAN_RECOVERED: A loop was removed on Ten-GigabitEthernet3/0/1 in VLAN 100.

%Feb 24 15:04:44:243 2019 DeviceA LPDT/5/LPDT_RECOVERED: All loops were removed on Ten-GigabitEthernet3/0/1.

%Feb 24 15:04:44:248 2019 DeviceA LPDT/5/LPDT_VLAN_RECOVERED: A loop was removed on Ten-GigabitEthernet3/0/2 in VLAN 100.

%Feb 24 15:04:44:248 2019 DeviceA LPDT/5/LPDT_RECOVERED: All loops were removed on Ten-GigabitEthernet3/0/2.

The output shows the following information:

·     Device A detected loops on Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 within a loop detection interval.

·     Loops on Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 were removed.

# Use the display loopback-detection command to display the loop detection configuration and status on devices, for example, Device A.

[DeviceA] display loopback-detection

Loop detection is enabled.

Global loop detection interval is 35 second(s).

Loop is detected on following interfaces:

  Interface                      Action mode     VLANs/VSI

 Ten-GigabitEthernet3/0/1       Shutdown        100

 Ten-GigabitEthernet3/0/2       Shutdown        100

The output shows that the device has removed the loops from Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 according to the shutdown action.

# Display the status of Ten-GigabitEthernet 3/0/1 on devices, for example, Device A.

[DeviceA] display interface ten-gigabitethernet 3/0/1

Ten-GigabitEthernet3/0/1 current state: DOWN (Loop detection down)

...

The output shows that Ten-GigabitEthernet 3/0/1 is already shut down by the loop detection module.

# Display the status of Ten-GigabitEthernet 3/0/2 on devices, for example, Device A.

[DeviceA] display interface ten-gigabitethernet 3/0/2

Ten-GigabitEthernet3/0/2 current state: DOWN (Loop detection down)

...

The output shows that Ten-GigabitEthernet 3/0/2 is already shut down by the loop detection module.

Example: Configuring loop detection on a M-LAG system

Network configuration

As shown in Figure 4, configure loop detection on the M-LAG system formed by Device A and Device B to meet the following requirements:

·     Generates a log as a notification.

·     Automatically shuts down the interface on which a loop is detected.

Figure 4 Network diagram

 

Procedure

1.     Configure Device A:

# Create VLAN 100.

<DeviceA> system-view

[DeviceA] vlan 100

[DeviceA-vlan100] quit

# Configure M-LAG system settings.

[DeviceA] m-lag system-mac 1-1-1

[DeviceA] m-lag system-number 1

[DeviceA] m-lag system-priority 123

# Configure M-LAG keepalive packet parameters.

[DeviceA] m-lag keepalive ip destination 1.1.1.1 source 1.1.1.2

# Set the link mode of Ten-GigabitEthernet 3/0/6 to Layer 3, and assign the interface an IP address. The IP address will be used as the source IP address of keepalive packets.

[DeviceA] interface ten-gigabitethernet 3/0/6

[DeviceA-Ten-GigabitEthernet3/0/6] port link-mode route

[DeviceA-Ten-GigabitEthernet3/0/6] ip address 1.1.1.2 24

[DeviceA-Ten-GigabitEthernet3/0/6] quit

# Exclude the interface used for M-LAG keepalive detection (Ten-GigabitEthernet 3/0/6) from the shutdown action by M-LAG MAD.

[DeviceA] m-lag mad exclude interface ten-gigabitethernet 3/0/6

# Create Layer 2 dynamic aggregate interface Bridge-Aggregation 3, and specify it as the M-LAG peer-link interface.

[DeviceA] interface bridge-aggregation 3

[DeviceA-Bridge-Aggregation3] link-aggregation mode dynamic

[DeviceA-Bridge-Aggregation3] port m-lag peer-link 1

[DeviceA-Bridge-Aggregation3] quit

# Assign Ten-GigabitEthernet 3/0/5 to aggregation group 3.

[DeviceA] interface ten-gigabitethernet 3/0/5

[DeviceA-Ten-GigabitEthernet3/0/5] port link-aggregation group 3

[DeviceA-Ten-GigabitEthernet3/0/5] quit

# Set the link type of Bridge-Aggregation 3 to trunk, and assign it to VLAN 100.

[DeviceA] interface bridge-aggregation 3

[DeviceA-Bridge-Aggregation3] port link-type trunk

[DeviceA-Bridge-Aggregation3] port trunk permit vlan 100

[DeviceA-Bridge-Aggregation3] quit

# Create Layer 2 dynamic aggregate interface Bridge-Aggregation 4, and assign it to M-LAG group 4.

[DeviceA] interface bridge-aggregation 4

[DeviceA-Bridge-Aggregation4] link-aggregation mode dynamic

[DeviceA-Bridge-Aggregation4] port m-lag group 4

[DeviceA-Bridge-Aggregation4] quit

# Assign Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 to aggregation group 4.

[DeviceA] interface ten-gigabitethernet 3/0/1

[DeviceA-Ten-GigabitEthernet3/0/1] port link-aggregation group 4

[DeviceA-Ten-GigabitEthernet3/0/1] quit

[DeviceA] interface ten-gigabitethernet 3/0/2

[DeviceA-Ten-GigabitEthernet3/0/2] port link-aggregation group 4

[DeviceA-Ten-GigabitEthernet3/0/2] quit

# Set the link type of Bridge-Aggregation 4 to trunk, and assign it to VLAN 100.

[DeviceA] interface bridge-aggregation 4

[DeviceA-Bridge-Aggregation4] port link-type trunk

[DeviceA-Bridge-Aggregation4] port trunk permit vlan 100

[DeviceA-Bridge-Aggregation4] quit

# Create Layer 2 dynamic aggregate interface Bridge-Aggregation 5, and assign it to M-LAG group 5.

[DeviceA] interface bridge-aggregation 5

[DeviceA-Bridge-Aggregation5] link-aggregation mode dynamic

[DeviceA-Bridge-Aggregation5] port m-lag group 5

[DeviceA-Bridge-Aggregation5] quit

# Assign Ten-GigabitEthernet 3/0/3 and Ten-GigabitEthernet 3/0/4 to aggregation group 5.

[DeviceA] interface ten-gigabitethernet 3/0/3

[DeviceA-Ten-GigabitEthernet3/0/3] port link-aggregation group 5

[DeviceA-Ten-GigabitEthernet3/0/3] quit

[DeviceA] interface ten-gigabitethernet 3/0/4

[DeviceA-Ten-GigabitEthernet3/0/4] port link-aggregation group 5

[DeviceA-Ten-GigabitEthernet3/0/4] quit

# Set the link type of Bridge-Aggregation 5 to trunk, and assign it to VLAN 100.

[DeviceA] interface bridge-aggregation 5

[DeviceA-Bridge-Aggregation5] port link-type trunk

[DeviceA-Bridge-Aggregation5] port trunk permit vlan 100

[DeviceA-Bridge-Aggregation5] quit

# Disable the spanning tree feature.

[DeviceA] undo stp global enable

# Enable loop detection for VLAN 100 globally, set the global loop protection action to shutdown, and set the loop detection interval to 35 seconds.

[DeviceA] loopback-detection global enable vlan 100

[DeviceA] loopback-detection global action shutdown

[DeviceA] loopback-detection interval-time 35

2.     Configure Device B in the same way Device A is configured. Set the M-LAG system number to 2, and set the source and destination IP addresses of keepalive packets to 1.1.1.1 and 1.1.1.2, respectively. (Details not shown.)

3.     Configure Device C:

# Disable the spanning tree feature.

<DeviceC> system-view

[DeviceC] undo stp global enable

# Create VLAN 100.

[DeviceC] vlan 100

[DeviceC-vlan100] quit

# Create Layer 2 dynamic aggregate interface Bridge-Aggregation 4.

[DeviceC] interface bridge-aggregation 4

[DeviceC-Bridge-Aggregation4] link-aggregation mode dynamic

[DeviceC-Bridge-Aggregation4] quit

# Assign Ten-GigabitEthernet 3/0/1 through Ten-GigabitEthernet 3/0/4 to aggregation group 4.

[DeviceC] interface range ten-gigabitethernet 3/0/1 to ten-gigabitethernet 3/0/4

[DeviceC-if-range] port link-aggregation group 4

[DeviceC-if-range] quit

# Set the link type of Bridge-Aggregation 4 to trunk, and assign it to VLAN 100.

[DeviceC] interface bridge-aggregation 4

[DeviceC-Bridge-Aggregation4] port link-type trunk

[DeviceC-Bridge-Aggregation4] port trunk permit vlan 100

[DeviceC-Bridge-Aggregation4] quit

# Set the link type of Ten-GigabitEthernet 3/0/5 to trunk, and assign it to VLAN 100.

[DeviceC] interface ten-gigabitethernet 3/0/5

[DeviceC-Ten-GigabitEthernet3/0/5] port link-type trunk

[DeviceC-Ten-GigabitEthernet3/0/5] port trunk permit vlan 100

[DeviceC-Ten-GigabitEthernet3/0/5] quit

4.     Configure Device D:

# Disable the spanning tree feature.

<DeviceD> system-view

[DeviceD] undo stp global enable

# Create VLAN 100.

[DeviceD] vlan 100

[DeviceD-vlan100] quit

# Create Layer 2 dynamic aggregate interface Bridge-Aggregation 5.

[DeviceD] interface bridge-aggregation 5

[DeviceD-Bridge-Aggregation5] link-aggregation mode dynamic

[DeviceD-Bridge-Aggregation5] quit

# Assign Ten-GigabitEthernet 3/0/1 through Ten-GigabitEthernet 3/0/4 to aggregation group 5.

[DeviceD] interface range ten-gigabitethernet 3/0/1 to ten-gigabitethernet 3/0/4

[DeviceD-if-range] port link-aggregation group 5

[DeviceD-if-range] quit

# Set the link type of Bridge-Aggregation 5 to trunk, and assign it to VLAN 100.

[DeviceD] interface bridge-aggregation 5

[DeviceD-Bridge-Aggregation5] port link-type trunk

[DeviceD-Bridge-Aggregation5] port trunk permit vlan 100

[DeviceD-Bridge-Aggregation5] quit

# Set the link type of Ten-GigabitEthernet 3/0/5 to trunk, and assign it to VLAN 100.

[DeviceD] interface ten-gigabitethernet 3/0/5

[DeviceD-Ten-GigabitEthernet3/0/5] port link-type trunk

[DeviceD-Ten-GigabitEthernet3/0/5] port trunk permit vlan 100

[DeviceD-Ten-GigabitEthernet3/0/5] quit

5.     Configure Device E:

# Disable the spanning tree feature.

<DeviceE> system-view

[DeviceE] undo stp global enable

# Create VLAN 100.

[DeviceE] vlan 100

[DeviceE-vlan100] quit

# Set the link type of Ten-GigabitEthernet 3/0/1 and Ten-GigabitEthernet 3/0/2 to trunk, and assign them to VLAN 100.

[DeviceE] interface ten-gigabitethernet 3/0/1

[DeviceE-Ten-GigabitEthernet3/0/1] port link-type trunk

[DeviceE-Ten-GigabitEthernet3/0/1] port trunk permit vlan 100

[DeviceE-Ten-GigabitEthernet3/0/1] quit

[DeviceE] interface ten-gigabitethernet 3/0/2

[DeviceE-Ten-GigabitEthernet3/0/2] port link-type trunk

[DeviceE-Ten-GigabitEthernet3/0/2] port trunk permit vlan 100

[DeviceE-Ten-GigabitEthernet3/0/2] quit

Verifying the configuration

# View the system logs on Device A.

[DeviceA]

%Aug  1 03:28:48:110 2019 DeviceA LPDT/4/LPDT_LOOPED: A loop was detected on

 Bridge-Aggregation4.

%Aug  1 03:28:48:191 2019 DeviceA LPDT/4/LPDT_VLAN_LOOPED: A loop was detect

ed on Bridge-Aggregation4 in VLAN 100.

%Aug  1 03:28:48:194 2019 DeviceA LPDT/4/LPDT_LOOPED: A loop was detected on

 Bridge-Aggregation5.

%Aug  1 03:28:48:288 2019 DeviceA LPDT/4/LPDT_VLAN_LOOPED: A loop was detect

ed on Bridge-Aggregation5 in VLAN 100.

%Aug  1 03:28:48:290 2019 DeviceA LPDT/5/LPDT_VLAN_RECOVERED: A loop was rem

oved on Bridge-Aggregation4 in VLAN 100.

%Aug  1 03:28:48:291 2019 DeviceA LPDT/5/LPDT_RECOVERED: All loops were remo

ved on Bridge-Aggregation4.

%Aug  1 03:28:48:302 2019 DeviceA LPDT/5/LPDT_VLAN_RECOVERED: A loop was rem

oved on Bridge-Aggregation5 in VLAN 100.

%Aug  1 03:28:48:304 2019 DeviceA LPDT/5/LPDT_RECOVERED: All loops were remo

ved on Bridge-Aggregation5.

The output shows the following information:

·     Device A detected loops on Bridge-Aggregation 4 and Bridge-Aggregation 5 within a loop detection interval.

·     Loops on Bridge-Aggregation 4 and Bridge-Aggregation 5 were removed.

# Use the display loopback-detection command to display the loop detection configuration and status on Device A.

[DeviceA] display loopback-detection

Loop detection is enabled.

Global loop detection interval is 35 second(s).

Loop is detected on following interfaces:

  Interface                       Action mode     VLANs/VSI

  Bridge-Aggregation4             Shutdown        100

  Bridge-Aggregation5             Shutdown        100

The output shows that the device has removed the loops from Bridge-Aggregation 4 and Bridge-Aggregation 5 according to the shutdown action.

# Verify that Bridge-Aggregation 4 has been shut down by loop detection.

[DeviceA] display interface Bridge-Aggregation 4

Bridge-Aggregation4

Current state: DOWN (Loopback detection down)

# Verify that Bridge-Aggregation 5 has been shut down by loop detection.

[DeviceA] display interface Bridge-Aggregation 5

Bridge-Aggregation5

Current state: DOWN (Loopback detection down)

# Verify that loops have been removed on Device B. (Details not shown.)

 

 

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Intelligent Storage
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
  • Technical Blogs
All Support
  • Become A Partner
  • Partner Policy & Program
  • Global Learning
  • Partner Sales Resources
  • Partner Business Management
  • Service Business
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us