H3C S3610[S5510] Series Ethernet Switches Command Manual-Release 5301-(V1.03)
HomeSupportSwitchesH3C S3610[S5510] Switch SeriesReference GuidesCommand ReferencesH3C S3610[S5510] Series Ethernet Switches Command Manual-Release 5301-(V1.03)
31-NQA Commands
31-NQA Commands 131 KB
Chapter 1  NQA Configuration Commands
1.1  NQA Client Commands
1.1.1  count
count times
undo count
View
NQA test group view
times: Number of probes in a test, in the range 1 to 15.
Use the count command to configure the number of probes in a test.
Use the undo count command to restore the default.
By default, one probe is performed in a test.
For a TCP test, one probe means one connection; for a Jitter test, the number of packets sent in one probe depends on the jitter-packetnum command; for an SNMP test, three packets are sent in one probe; for other types of tests, one packet is sent for one probe.
If the number of probes in a test is greater than 1, the system sends a second packet after it sends the first packet and receives a response packet. If the system does not receive a response packet, the system waits for the test timer to expire before sending a second test packet. The process is repeated until the specified probes are completed.
# Configure the number of probes in a test as 10.
[Sysname] nqa administrator test
[Sysname-nqa-administrator-test] count 10
1.1.2  datafill
datafill text
undo datafill
View
NQA test group view
text: String of fill characters of a test packet, in the range 1 to 200.
Use the datafill command to configure the string of fill characters for a test packet.
Use the undo datafill command to restore the default.
By default, the string of fill characters of an ICMP packet is the string corresponding with the ASCII code 00 to 09 and that for a UDP packet is the string corresponding with the ASCII code 00 to FF.
The fill data of an NQA test packet can be any string of characters. If the test packet is smaller than the fill data, the system uses only the first part of the character string to encapsulate the packet. If the test packet is larger than the fill data, the system fills the character string cyclically to encapsulate the test packet until the packet is full. For example, when the fill data is abcd and the size of a test packet is 3 byte, abc is used to fill. When the test packet size is 6 byte, abcdab is used to fill.
Because the first byte of a UDP packet has some specific usage, the configured character string is used to fill the remaining bytes in the packet.
Note that the datafill command is valid for an ICMP test and a UDP test.
# Configure the string of fill characters of a test packet as abcd.
[Sysname-nqa-administrator-test] datafill abcd
1.1.3  datasize
datasize size
undo datasize
View
NQA test group view
size: Size of a test packet in bytes, in the range of 1 to 8100.
Use the datasize command to configure the size of a test packet, namely, an echo request packet (IP header and ICMP header excluded).
Use the undo datasize command to restore the size of a test request packet to the default value.
By default, the size of an ICMP test packet is 56 bytes and that of a UDP test packet is 100 bytes.
Note that:
l           The datasize command is valid only for ICMP and UDP tests.
l           For an ICMP test, if the value of the size argument is less than 20, the system automatically fills ICMP test packets to 20 bytes with a string of fill characters.
l           When you perform a UDP test, the size of test packets is subject to the configuration.
Related commands: datafill.
# Configure the size of a test packet as 50 bytes.
[Sysname-nqa-administrator-test] datasize 50
1.1.4  description
View
NQA test group view
text: Descriptive string of characters for a test group, in the range 1 to 200.
Use the description command to give a brief description of a test group, usually, the test type or test purpose of a test group.
Use the undo description command to remove the description information.
By default, no descriptive string is available for a test group.
# Configure a descriptive string for a test group as icmp-test.
[Sysname-nqa-administrator-test] description icmp-test
1.1.5  destination-ip
destination-ip ip-address
undo destination-ip
View
NQA test group view
ip-address: Destination IP address of a test request packet.
Use the destination-ip command to configure a destination IP address for a test request packet.
Use the undo destination-ip command to remove the destination IP address.
By default, no destination IP address is configured for a test request packet.
Related commands: destination-port.
# Set the destination IP address of a test request packet to 10.1.1.1.
[Sysname-nqa-administrator-test] destination-ip 10.1.1.1
1.1.6  destination-port
destination-port port-number
undo destination-port
View
NQA test group view
port-number: Destination port number of a test request packet, in the range 1 to 65535.
Use the destination-port command to configure a destination port number for a test request packet.
Use the undo destination-port command to remove the destination port number.
By default, no destination port number is configured for a test request packet.
Related commands: destination-ip
&  Note:
l      The destination-port command is applicable to only jitter, TCP-Private, and UDP-Private tests.
l      You are not recommended to perform a TCP, UDP, or jitter test on port from 1 to 1023 (known ports). Otherwise, the NQA test will fail or the corresponding services of this port will be unavailable.
# Set the destination port number of a test request packet to 9000.
[Sysname-nqa-administrator-test] destination-port 9000
1.1.7  display nqa
display nqa { results | history | jitter } [ admin-name operation-tag ]
View
results: Displays the results of the last test.
history: Displays the history records of tests.
jitter: Displays the recorded delay jitter of UDP packet transmission in the last NQA jitter test.
admin-name operation-tag: Displays information of the specified NQA test group. admin-name represents the name of the administrator who creates NQA test groups and is a string of 1 to 32 characters. operation-tag represents the test operation tag and is a string of 1 to 32 characters.
Use the display nqa command to display results of an NQA test or tests.
If neither of the test group arguments (admin-name and operation-tag) is specified, results of all test groups are displayed. Otherwise, results of only the specified test group(s) are displayed.
Related commands: test-enable.
# Display the results of the last test.
<Sysname> display nqa results administrator icmp
  NQA entry(admin administrator, tag icmp) test result:
      Destination ip address: 169.254.10.2
      Send operation times: 10             Receive response times: 10
      Min/Max/Average Round Trip Time: 1/2/1
      Square-Sum of Round Trip Time: 13
      Last succeeded test time: 2004-11-25 16:28:55.0
    Extend result:
      Packet lost in test: 0%
      Failures due to Timeout: 0
      Failures due to System Busy: 0
      Failures due to Disconnect: 0
      Failures due to No Connection: 0
      Failures due to Sequence Error: 0
      Failures due to Internal Error: 0
      Failures due to Other Errors: 0
Table 1-1 Description on the fields of the display nqa results command
IP address of the destination
Number of probe packets sent
Number of response packets received
Minimum/maximum/average roundtrip time
Square sum of roundtrip time
Completion time of the last successful test
SD Maximal delay
Maximum delay from the source to the destination
DS Maximal delay
Maximum delay from the destination to the source
Packet lost in test
Average packet loss ratio
Disconnect operation number
Number of disconnections by the peer
Number of time-out occurrences in a test
Number of test failures owing to the system being busy
Number of failures to connect with the peer
Number of failures owing to out-of-sequence packets
Number of failures owing to internal errors
Number of failures owing to other errors
# Display the history records of tests.
<Sysname> display nqa history administrator test
  NQA entry(admin administrator, tag test) history record:
    Index     Response    Status      LastRC      Time
        1            1         1           0    2004-11-25 16:28:55.0
        2            1         1           0    2004-11-25 16:28:55.0
        3            1         1           0    2004-11-25 16:28:55.0
        4            1         1           0    2004-11-25 16:28:55.0
        5            1         1           0    2004-11-25 16:28:55.0
        6            2         1           0    2004-11-25 16:28:55.0
        7            1         1           0    2004-11-25 16:28:55.0
        8            1         1           0    2004-11-25 16:28:55.0
        9            1         1           0    2004-11-25 16:28:55.9
       10            1         1           0    2004-11-25 16:28:55.9
Table 1-2 Description on the fields of the display nqa history command
Index
History record number
Response
Roundtrip delay of a test packet in the case of a successful test, time-out time in the case of time-out, or 0 in the case of a test failure (in milliseconds)
Status
Status value of test results, including:
1: responseReceived
2: unknown
3: internalError
4: requestTimedOut
5: unknownDestinationAddress
6: noRouteToTarget
7: interfaceInactiveToTarget
8: arpFailure
9: maxConcurrentLimitReached
10: unableToResolveDnsName
11: invalidHostAddress
LastRC
Temporarily, this field is not supported.
Time
Time when the test is completed
# Display the recorded delay jitter of UDP packet transmission in the last NQA jitter test.
<Sysname> display nqa jitter admin jitter
  NQA entry(admin admin, tag jitter) test jitter result:
      RTT Number: 10
      SD Maximal delay: 2                  DS Maximal delay: 2
      Min Positive SD: 1                   Min Positive DS: 1
      Max Positive SD: 1                   Max Positive DS: 1
      Positive SD Number: 4                Positive DS Number: 2
      Positive SD Sum: 4                   Positive DS Sum: 2
      Positive SD average: 1               Positive DS average: 1
      Positive SD Square Sum: 4            Positive DS Square Sum: 2
      Min Negative SD: 1                   Min Negative DS: 1
      Max Negative SD: 2                   Max Negative DS: 1
      Negative SD Number: 2                Negative DS Number: 3
      Negative SD Sum: 3                   Negative DS Sum: 3
      Negative SD average: 2               Negative DS average: 1
      Negative SD Square Sum: 5            Negative DS Square Sum: 3
      SD lost packets number: 0            DS lost packet number: 0
      Unknown result lost packet number: 0
Table 1-3 Description on the fields of the display nqa jitter command
RTT Number
Number of received response packets
SD Maximal delay
DS Maximal delay
Min Positive SD
Minimum positive jitter delay from the source to the destination
Min Positive DS
Minimum positive jitter delay from the destination to the source
Max Positive SD
Maximum positive jitter delay from the source to the destination
Max Positive DS
Maximum positive jitter delay from the destination to the source
Positive SD Number
Number of positive jitter delays from the source to the destination
Positive DS Number
Number of positive jitter delays from the destination to the source
Positive SD Sum
Sum of positive jitter delays from the source to the destination
Positive DS Sum
Sum of positive jitter delays from the destination to the source
Positive SD average
Average of positive jitter delays from the source to the destination
Positive DS average
Average of positive jitter delays from the destination to the source
Sum of the square of positive jitter delays from the source to the destination
Sum of the square of positive jitter delays from the destination to the source
Min Negative SD
Minimum absolute value of negative jitter delays from the source to the destination
Min Negative DS
Minimum absolute value of negative jitter delays from the destination to the source
Max Negative SD
Maximum absolute value of negative jitter delays from the source to the destination
Max Negative DS
Maximum absolute value of negative jitter delays from the destination to the source
Negative SD Number
Number of negative jitter delays from the source to the destination
Negative DS Number
Number of negative jitter delays from the destination to the source
Negative SD Sum
Sum of absolute values of negative jitter delays from the source to the destination
Negative DS Sum
Sum of absolute values of negative jitter delays from the destination to the source
Negative SD average
Average of negative jitter delays from the source to the destination
Negative DS average
Average of negative jitter delays from the destination to the source
Sum of the square of negative jitter delays from the source to the destination
Sum of the square of negative jitter delays from the destination to the source
Number of lost packets from the source to the destination
Number of lost packets from the destination to the source
Number of lost packets for unknown reasons
1.1.8  filename
filename file-name
undo filename
View
NQA test group view
file-name: Name of the file transferred between the FTP server and the FTP client, a string of 1 to 200 characters.
Use the filename command to specify a file to be transferred between the FTP server and the FTP client.
Use the undo filename command to cancel the file.
By default, no file is specified.
Note that the filename command is valid only for FTP tests.
Related commands: username, password, and ftp-operation.
# Specify the config.txt file to be transferred between the FTP server and the FTP client.
[Sysname-nqa-administrator-test] filename config.txt
1.1.9  frequency
frequency interval
undo frequency
View
NQA test group view
interval: Interval of performing a cyclic test in seconds, in the range 1 to 65535.
Use the frequency command to configure the interval of performing a cyclic test. After you execute the test-enable command to start an NQA test, the test will be performed at intervals.
Use the undo frequency command to restore the default.
By default, no cyclic test is performed.
Note that the frequency command is invalid for the DHCP test.
# Configure the interval of performing a cyclic test as 10 seconds.
[Sysname-nqa-administrator-test] frequency 10
1.1.10  ftp-operation
ftp-operation { get | put }
undo ftp-operation
View
NQA test group view
get: Obtains a file from the FTP server.
put: Transfers a file to the FTP server.
Use the ftp-operation command to configure the FTP operation type.
Use the undo ftp-operation command to restore the default.
By default, the FTP operation type is “get” (obtain a file from the FTP server).
Note that the ftp-operation command is valid only for FTP tests.
Related commands: username, password.
# Obtain a file from the FTP server.
[Sysname-nqa-administrator-test] ftp-operation get
1.1.11  history-records
history-records number
undo history-records
View
NQA test group view
number: Maximum number of history records that can be saved in a test group, in the range 0 to 50.
Use the history-records command to configure the maximum number of history records that can be saved in a test group.
Use the undo history-records command to restore the default.
By default, the maximum number of records that can be saved in a test group is 50.
If the history records exceed the predefined maximum number, the first test result will be discarded.
# Configure the maximum number of history records that can be saved in a test group as 10.
[Sysname-nqa-administrator-test] history-records 10
1.1.12  http-operation
http-operation { get | post }
undo http-operation
View
NQA test group view
get: Obtains data from the HTTP server.
post: Transfers data to the HTTP server.
Use the http-operation command to configure the HTTP operation type.
Use the undo http-operation command to restore the default.
By default, the HTTP operation type is get (obtain data from the HTTP server).
Note that the http-operation command is valid only for HTTP tests.
Related commands: http-string.
# Obtain data from the HTTP server.
[Sysname-nqa-administrator-test] http-operation get
1.1.13  http-string
http-string string version
undo http-string
View
NQA test group view
string: HTTP operation string, which specifies a webpage to be accessed. The length of the string argument plus that of the version argument must be less than 200 characters.
version: HTTP version. Currently, it can only be “HTTP/1.0”, where HTTP must be capital.
Use the http-string command to configure an HTTP operation string and version information.
Use the undo http-string command to remove the configuration of the HTTP operation string and version information.
By default, no HTTP operation string or version information is configured.
Note that the http-string command is valid only for HTTP tests.
Related commands: http-operation.
# Set the web page accessible through HTTP to /index.htm and the HTTP version to HTTP/1.0.
[Sysname-nqa-administrator-test] http-string /index.htm HTTP/1.0
1.1.14  nqa
nqa admin-name operation-tag
undo nqa admin-name operation-tag
View
admin-name: Name of the administrator who creates NQA test groups, a string of 1 to 32 characters.
operation-tag: Tag of a test operation, a string of 1 to 32 characters.
Use the nqa command to create an NQA test group and enter its view. If the test group already exists, you will directly enter NQA test group view when you execute the nqa command.
Use the undo nqa command to remove the test group.
# Create an NQA test group whose administrator name is administrator and whose operation tag is test and enter NQA test group view.
1.1.15  nqa-agent enable
nqa-agent enable
undo nqa-agent enable
View
None
Use the nqa-agent enable command to enable the NQA client.
Use the undo nqa-agent enable command to disable the NQA client.
By default, the NQA client is disabled.
Note that you can perform tests only after the NQA client is enabled.
Related commands: nqa-server enable.
# Enable the NQA client.
[Sysname] nqa-agent enable
1.1.16  nqa-agent max-requests
nqa-agent max-requests max-number
undo nqa-agent max-requests
View
max-number: Maximum number of tests that the NQA client can simultaneously perform, in the range 1 to 5.
Use the nqa-agent max-requests command to configure the maximum number of tests that the NQA client can simultaneously perform.
Use the undo nqa-agent max-requests command to restore the default.
By default, the maximum number of tests that the NQA client can simultaneously perform is five.
# Specify the NQA client to simultaneously perform four tests at most.
[Sysname] nqa-agent max-requests 4
1.1.17  jitter-interval
jitter-interval interval
undo jitter-interval
View
NQA test group view
interval: Interval for sending jitter test packets in milliseconds, in the range 10 to 1,000.
Use the jitter-interval command to configure the interval of sending jitter test packets.
Use the undo jitter-interval command to restore the default.
By default, the interval for sending jitter test packets is 20 milliseconds.
Note that the jitter-interval command is valid only for a jitter test.
Related commands: jitter-packetnum.
# Set the interval of sending jitter test packets to 30 milliseconds.
[Sysname-nqa-administrator-test] jitter-interval 30
1.1.18  jitter-packetnum
jitter-packetnum number
undo jitter-packetnum
View
NQA test group view
number: Number of test packets sent in a probe, in the range 10 to 100.
Use the jitter-packetnum command to configure the number of jitter test packets sent in a probe.
Use the undo jitter-packetnum command to restore the default.
By default, the number of test packets sent in a probe is 10.
Note that the jitter-packetnum command is valid only for a jitter test.
Related commands: jitter-interval.
# Set the number of packets sent in a probe to 30.
[Sysname-nqa-administrator-test] jitter-packetnum 30
1.1.19  password
password password
undo password
View
NQA test group view
password: Password used to log on to the FTP server, a string of 1 to 32 characters.
Use the password command to configure a password used to log onto the FTP server.
Use the undo password command to remove the password.
By default, no password is configured.
Note that the password command is valid only for an FTP test.
Related commands: username and ftp-operation.
# Set the login password to nqa.
[Sysname-nqa-administrator-test] test-type ftp
[Sysname-nqa-administrator-test] username aaa
[Sysname-nqa-administrator-test] password nqa
1.1.20  probe-failtimes
probe-failtimes times
undo probe-failtimes
View
NQA test group view
times: Number of consecutive probe failures in a test, in the range 1 to 15.
Use the probe-failtimes command to configure the number of consecutive probe failures in an NQA test before a trap message is sent to the network management server to indicate a probe failure.
Use the undo probe-failtimes command to restore the default.
By default, a Trap message is sent to the network management (NM) server once one probe fails in an NQA test.
&  Note:
l      One test may involve multiple probes.
l      Currently, the device does not support Trap message delivery. Therefore the configured probe-failtimes or undo probe-failtimes command does not take effect.
# Configure the system to send a Trap message after three consecutive probe failures in an NQA test.
[Sysname-nqa-administrator-test] probe-failtimes 3
1.1.21  send-trap
send-trap { all | { probefailure | testcomplete | testfailure }* }
undo send-trap { all | { probefailure | testcomplete | testfailure }* }
View
NQA test group view
probefailure: Sends a Trap message when a probe fails.
testcomplete: Sends a Trap message when a test is completed.
testfailure: Sends a Trap message when a test fails (the number of probe failures in a test is greater than or equal to the number configured by the test-failtimes command). For a test, only one trap message is sent.
all: Sends a Trap message in any of the above cases.
Use the send-trap command to enable the Trap debugging (A Trap message is sent to the network management server).
Use the undo send-trap command to disable the Trap debugging (No Trap message is sent to the network management server).
By default, no trap message is sent to the network management server.
&  Note:
Currently, the device does not support Trap message delivery. Therefore the configured send-trap or undo send-trap command does not take effect.
# Send a Trap message when a test is completed.
[Sysname-nqa-administrator-test] send-trap testcomplete
1.1.22  sendpacket passroute
undo sendpacket passroute
View
NQA test group view
None
Use the sendpacket passroute command to enable the routing table bypass function to test the direct connectivity to the destination.
Use the undo sendpacket passroute command to disable the routing table bypass function.
By default, the routing table bypass function is disabled.
After this function is enabled, the routing table is not searched, and the packet is directly sent to the destination in a directly connected network. If the destination is not in the directly connected network, an error will be prompted.
Note that the sendpacket passroute command is invalid for DHCP tests.
# Enable the routing table bypass function.
[Sysname-nqa-administrator-test] sendpacket passroute
1.1.23  source-interface
source-interface interface-type interface-number
undo source-interface
View
NQA test group view
interface-type interface-number: Specifies the interface by its type and number.
Use the source-interface command to specify the IP address of an interface as the source IP address of ICMP test request packets or specify an interface for a DHCP test.
Use the undo source-interface command to remove the configuration.
By default, no interface address is specified as the source IP address of ICMP test request packets, or no interface is specified for a DHCP test.
Note that:
l           For a DHCP test, the source-interface command is required, for an ICMP test, it is optional, and for other tests, it is invalid.
l           For an ICMP test, if a source IP address is configured by using the source-ip command, the configuration by using the source-interface command is invalid.
l           The interface specified by the source-interface command can only be VLAN interface.
l           The interface specified by the command must be up. Otherwise, the test will fail.
# Specify Ethernet 1/0 for a DHCP test.
[Sysname-nqa-administrator-test] test-type dhcp
[Sysname-nqa-administrator-test] source-interface ethernet 1/0
1.1.24  source-ip
source-ip ip-address
undo source-ip
View
NQA test group view
ip-address: Source IP address of a test request packet.
Use the source-ip command to configure a source IP address for a test request packet.
Use the undo source-ip command to remove the configured source address. That is, the IP address of the interface sending a test request packet serves as the source IP address of the test request packet.
By default, no source IP address is specified. If a source interface is specified, the IP address of the source interface serves as the source IP address of a test request packet.
Note that:
l           For an FTP test, the source-ip command is required, for a DHCP test, it is invalid, and for other tests, it is optional.
l           The source IP address in the command must be the IP address of an interface on the device and the interface must be up. Otherwise, the test will fail.
# Configure the source IP address of a test request packet as 10.1.1.1.
[Sysname-nqa-administrator-test] source-ip 10.1.1.1
1.1.25  source-port
source-port port-number
undo source-port
View
NQA test group view
port-number: Source port number for a test request packet, in the range 1 to 50000.
Use the source-port command to configure a source port number for a test request packet.
Use the undo source-port command to remove the configured port number.
By default, no source port number is specified.
Note that this command is valid only for jitter, UDP, and SNMP tests.
# Configure the source port number of a test request packet as 8000.
[Sysname-nqa-administrator-test] source-port 8000
1.1.26  test-type
test-type test-type
undo test-type
View
NQA test group view
test-type: Type of a test, including the following keywords:
l           dhcp: DHCP test.
l           dlsw: DLSw test.
l           ftp: FTP test.
l           http: HTTP test.
l           icmp: ICMP test.
l           jitter: Analyzes and tests the delay jitter of UDP packet transmission.
l           snmpquery: SNMP test.
l           tcpprivate: Tests the TCP connection to a specified port.
l           tcppublic: Tests the TCP connection to port 7.
l           udpprivate: Tests the UDP connection to a specified port.
l           udppublic: Tests the UDP connection to port 7.
Use the test-type command to configure the test type.
Use the undo test-type command to restore the default.
By default, the test type is ICMP.
# Set the test type to FTP.
1.1.27  test-enable
test-enable
undo test-enable
View
NQA test group view
None
Use the test-enable command to enable the NQA test.
Use the undo test-enable command to disable the NQA test.
Test results will not be displayed after you enable the NQA test. In this case, you need to execute the display nqa command to display the test results.
Related commands: display nqa.
# Enable the NQA test.
[Sysname-nqa-administrator-test] test-enable
1.1.28  test-failtimes
test-failtimes times
undo test-failtimes
View
NQA test group view
times: Minimum number of probe failures in a test before a Trap message is sent to indicate a test failure, in the range 1 to 15.
Use the test-failtimes command to configure the minimum number of probe failures in a test before a Trap message is sent to the network management server to indicate a test failure.
Use the undo test-failtimes command to restore the default.
By default, a Trap message is sent to the NM server once a probe fails in a test.
&  Note:
l      Currently, the device does not support Trap message delivery. Therefore the configured test-failtimes or undo test-failtimes command does not take effect.
# Configure the system to send a Trap message to indicate a test failure after three probe failures in an NQA test.
[Sysname-nqa-administrator-test] test-failtimes 3
1.1.29  timeout
timeout time
undo timeout
View
NQA test group view
time: Time-out time in one probe, in the range 1 to 60 seconds.
Use the timeout command to configure the time-out time in one probe. If no response packet is received within the time-out time of a request packet, the probe fails.
Use the undo timeout command to restore the default.
By default, the time-out time in one probe is three seconds.
# Configure the time-out time in one probe as 10 seconds.
[Sysname-nqa-administrator-test] timeout 10
1.1.30  tos
tos value
undo tos
View
NQA test group view
value: Value of the ToS field in the IP header in an NQA test packet, in the range 0 to 255.
Use the tos command to configure the value of the ToS field in the IP header in an NQA test packet.
Use the undo tos command to restore the default.
By default, the ToS field in the IP header of an NQA test packet is 0.
Note that the tos command is invalid for DHCP tests.
# Set the ToS field in the IP packet header in an NQA test packet to 1.
[Sysname-nqa-administrator-test] tos 1
1.1.31  ttl
ttl number
undo ttl
View
NQA test group view
number: Maximum number of hops a test request packet traverses in the network, in the range 1 to 255.
Use the ttl command to configure the maximum number of hops a test request packet traverses in the network.
Use the undo ttl command to restore the maximum number of hops to the default.
By default, the maximum number of hops that a test request packet can traverse in a network is 20.
&  Note:
l      The ttl command is invalid for DHCP tests.
l      After you configure the sendpacket passroute command, the maximum number of hops a test request packet traverses in the network is 1.
# Configure the maximum number of hops a test request packet traverses in the network as 16.
[Sysname-nqa-administrator-test] ttl 16
1.1.32  username
username name
undo username
View
NQA test group view
name: Username used to log on to the FTP server, a string of 1 to 32 characters.
Use the username command to configure a username used to log onto the FTP server.
Use the undo username command to remove the configured username.
By default, no username is configured.
Note that the username command is valid only for FTP tests.
Related commands: password and ftp-operation.
# Set the login username to administrator.
[Sysname-nqa-administrator-test] username administrator
1.1.33  vpninstance
vpninstance name
undo vpninstance
View
NQA test group view
name: VPN instance name, a string of 1 to 31 characters.
Use the vpninstance command to specify a VPN instance. If there are multiple VPNs, you need to use this command to specify a VPN for test.
Use the undo vpninstance command to remove the specified VPN instance.
By default, no VPN instance is specified.
Note that the vpninstance command is valid only for ICMP tests.
&  Note:
You can only use this command to specify an existing VPN instance.
# Specify the VPN instance vpn1.
[Sysname-nqa-administrator-test] vpninstance vpn1
1.2  NQA Server Commands
&  Note:
You only need to configure the NQA server for jitter, TCP, and UDP tests.
1.2.1  nqa-server enable
nqa-server enable
undo nqa-server enable
View
None
Use the nqa-server enable command to enable the NQA server.
Use the undo nqa-server enable command to disable the NQA server.
By default, the NQA server is disabled.
Related commands: nqa-agent enable, nqa-server tcpconnect, nqa-server udpecho.
# Enable the NQA server.
[Sysname] nqa-server enable
1.2.2  nqa-server tcpconnect
nqa-server tcpconnect ip-address port-number
undo nqa-server tcpconnect ip-address port-number
View
ip-address: IP address specified for the TCP listening service on the NQA server.
port-number: Port number specified for the TCP listening service on the NQA server, in the range 1 to 50000. For a TCP-Public test, the port number must be 7.
Use the nqa-server tcpconnect command to create a TCP listening service on the NQA server.
Use the undo nqa-server tcpconnect command to remove the TCP listening service from the NQA server.
Note that:
l           You need to configure the nqa-server tcpconnect command on the NQA server only for the TCP-Private and TCP-Public tests.
l           The IP address and port number must be consistent with those on the NQA client and must be different from those for an existing listening service.
l           The IP address must be that of an interface on the NQA server. Otherwise, the configuration will be invalid.
# Create a TCP listening service by using the IP address 169.254.10.2 and port 9000.
[Sysname] nqa-server tcpconnect 169.254.10.2 9000
1.2.3  nqa-server udpecho
nqa-server udpecho ip-address port-number
undo nqa-server udpecho ip-address port-number
View
ip-address: IP address specified for the UDP listening service on the NQA server.
port-number: Port number specified for the UDP listening service on the NQA server, in the range 1 to 50000. For the UDP-Public test, the port number must be 7.
Use the nqa-server udpecho command to create a UDP listening service on the NQA server.
Use the undo nqa-server udpecho command to remove the UDP connection.
Note that:
l           You need to configure the nqa-server udpecho command on the NQA server only for the jitter, UDP-Private, and UDP-Public tests.
l           The IP address and port number must be consistent with those of the NQA client and must be different from those of an existing listening service.
l           The IP address must be that of an interface on the NQA server and must not be 0.0.0.0. Otherwise, the configuration will be invalid.
# Create a UDP listening service by using the IP address 169.254.10.2 and port 9000.
[Sysname] nqa-server udpecho 169.254.10.2 9000
