- H3C Data Center Switches M-LAG Configuration Guide-6W101
- 00-M-LAG network planning
- 01-M-LAG+IPv4 and IPv6 Dual-Active VLAN Gateway Configuration Example
- 02-Multi-Layer M-LAG+STP+Dual-Active VLAN Gateway Configuration Examples
- 03-Multi-Layer M-LAG+Dual-Active VLAN Gateway+OSPF Configuration Examples
- 04-Multi-tier M-LAG+Spine Gateways+ECMP Paths to External Network Configuration Example
- 05-M-LAG and VRRP Configuration Example
- 06-M-LAG+RDMA Configuration Example
- 07-M-LAG and EVPN Distributed Gateway (IS-IS for underlay routing) Configuration Example
- 08-M-LAG and EVPN Distributed Gateway (BGP for Underlay Routing) Configuration Example
- 09-M-LAG+EVPN Distributed Gateway (OSPF on Underlay Network)+DHCP Relay+Microsegmentation+Service Chain Configuration Example
- 10-M-LAG+EVPN Centralized Gateway Configuration Example
- 11-Access to M-LAG Through Dynamic Routing and Distributed EVPN Gateways Configuration Example
- 12-M-LAG+EVPN+Monitor Link Configuration Examples
- 13-M-LAG and MVXLAN Configuration Example
- 14-M-LAG and DCI Configuration Example
- 15-M-LAG+EVPN DC Switchover Upon Border Failure Configuration Examples
- 16-Cascaded M-LAG Systems with Attached Multicast Source and Receivers Configuration Examples
| 05-M-LAG and VRRP Configuration Example | 395.80 KB |
Example: Configuring M-LAG and VRRP
Deploying a VRRP gateway on the M-LAG member devices
Configuring the links between the M-LAG member devices and the Layer 3 virtualization server
Configuring the links between the M-LAG member devices and core devices
Configuring BGP between the M-LAG member devices and core devices
Configuring BGP between the M-LAG member devices and the server
Configuring OSPF between the M-LAG member devices and the server
Configuring the links between the core devices and M-LAG member devices
Configuring the links between the core devices and the service network
Configuring BGP on the core devices for communication with the M-LAG member devices
Configuring OSPF on the core devices for communication with the service network
Underlay traffic forwarding models
Testing network convergence upon single points of failure
In the underlay network as shown in Figure 1, deploy M-LAG at the access layer to provide high availability and load balancing services for access devices. Deploy VRRP to provide gateway redundancy and ensure user service continuity. You can achieve the following purposes on the server through the VRRP gateway:
· To implement Layer 2 connectivity, the server can communicate with the service network at Layer 2 through the M-LAG system.
· Use the secondary IP addresses of the VLAN interfaces created on the M-LAG member devices to set up Layer 3 links between the server and the core devices, and configure BGP or OSPF to achieve Layer 3 connectivity.
Device role |
IP address |
Remarks |
M-LAG 1 |
WGE1/0/1 |
N/A |
Member port of an M-LAG interface. Connected to the server. |
WGE1/0/2 |
100.100.100.5/30 |
Connected to WGE1/0/2 on M-LAG 2 to establish the M-LAG keepalive link. |
HGE1/0/25 |
N/A |
Member port the peer-link interface. Connected to HGE1/0/25 on M-LAG 2. |
HGE1/0/26 |
N/A |
Member port the peer-link interface. Connected to HGE1/0/26 on M-LAG 2. |
HGE1/0/27 |
10.39.245.13/31 |
Connected to HGE1/0/2 on Core 2. |
HGE1/0/28 |
10.39.244.13/31 |
Connected to HGE1/0/1 on Core 1. |
Vlan-interface100 |
10.40.196.61/26 Secondary IP address: 100.127.128.253/24 Virtual IP address of the VRRP group: 10.40.196.1 10.40.196.1 |
Vlan-interface4094 |
100.100.100.1/30 |
Connects two M-LAG member devices over a Layer 3 link. |
Bridge-Aggregation 1 |
N/A |
Bridge-Aggregation 1024 |
N/A |
Peer-link interface. Connected to the peer link. |
M-LAG 2 |
WGE1/0/1 |
N/A |
Member port of the M-LAG interface. Connected to the server. |
WGE1/0/2 |
100.100.100.6/30 |
Connected to WGE1/0/2 on M-LAG 1. |
HGE1/0/25 |
N/A |
Member port of the peer-link interface. Connected to HGE1/0/25 on M-LAG 1. |
HGE1/0/26 |
N/A |
Member port of the peer-link interface. Connected to HGE1/0/26 on M-LAG 1. |
HGE1/0/27 |
10.39.244.45/31 |
Connected to HGE1/0/2 on Core 1. |
HGE1/0/28 |
10.39.245.45/31 |
Connected to HGE1/0/1 on Core 2. |
Vlan-interface100 |
10.40.196.62/26 Secondary IP address: 100.127.128.254/24 Virtual IP address of the VRRP group: 10.40.196.1 10.40.196.1 |
100.100.100.2/30 |
N/A |
N/A |
Core 1 |
HGE1/0/1 |
10.39.244.12/31 |
Connected to HGE1/0/28 on M-LAG 1. |
HGE1/0/2 |
10.39.244.44/31 |
Connected to HGE1/0/27 on M-LAG 2. |
HGE1/0/3 |
22.22.1.1/24 |
Connected to the service network. |
Core 2 |
HGE1/0/1 |
10.39.245.44/31 |
Connected to HGE1/0/28 on M-LAG 2. |
HGE1/0/2 |
10.39.245.12/31 |
Connected to HGE1/0/27 on M-LAG 1. |
HGE1/0/3 |
12.12.1.1/24 |
Analysis
· Deploy link aggregation between M-LAG 1 and the server and between M-LAG 2 and the server.
· Deploy M-LAG for M-LAG 1 and M-LAG 2 at the access layer. Configure a VRRP group and specify its virtual IP address as the gateway address of the server.
· Core 1 and Core 2 are Layer 3 devices connected to the service network.
· Create VLAN interfaces on the M-LAG interfaces of the M-LAG member devices, and configure the primary and secondary IP addresses.
¡ Set up Layer 3 links between the M-LAG member devices and the core devices, and configure BGP between them to achieve Layer 3 connectivity.
¡ Use the secondary IP address of the VLAN interfaces created on the M-LAG interfaces to set up Layer 3 links to the server, and configure BGP or OSPF to achieve Layer 3 connectivity.
Applicable product matrix
IMPORTANT: In addition to running an applicable software version, you must also install the most recent patch, if any. |
Device |
Software version |
S6805, S6825, S6850, S9850, S9820-64H, and S9820-8C |
R6710 |
S6800, S6860 |
R6710 |
S12500X-AF, S6890 |
R2825 |
S12500R |
R5210 |
S12500G-AF |
R7625 |
S6812, S6813 |
F6628P22 and higher |
Configuration procedure
Procedure summary
· Deploying a VRRP gateway on the M-LAG member devices
· Configuring the links between the M-LAG member devices and the Layer 3 virtualization server
· Configuring the links between the M-LAG member devices and core devices
· Configuring BGP between the M-LAG member devices and core devices
· Configure BGP or OSPF between the M-LAG member devices and the server (perform one of the following tasks):
¡ (Optional.) Configuring BGP between the M-LAG member devices and the server
¡ (Optional.) Configuring OSPF between the M-LAG member devices and the server
· Configuring the links between the core devices and M-LAG member devices
· Configuring the links between the core devices and the service network
· Configuring BGP on the core devices for communication with the M-LAG member devices
· Configuring OSPF on the core devices for communication with the service network
Configuring M-LAG
M-LAG 1 |
M-LAG 2 |
Remarks |
interface Bridge-Aggregation 1024 |
Create Layer 2 aggregate interface Bridge-Aggregation 1024. |
N/A |
link-aggregation mode dynamic |
Configure Bridge-Aggregation 1024 to operate in dynamic mode, and enable LACP. |
N/A |
quit |
quit |
N/A |
N/A |
interface range HundredGigE1/0/25 HundredGigE1/0/26 |
Enter peer link physical port view. |
N/A |
port link-aggregation group 1024 |
Assign the physical ports to Layer 2 aggregation group 1024. |
N/A |
quit |
quit |
N/A |
N/A |
interface Bridge-Aggregation1024 |
Enter the view of Bridge-Aggregation 1024 to be used as peer-link interface. |
N/A |
port m-lag peer-link 1 |
port m-lag peer-link1 |
Configure Bridge-Aggregation 1024 as the peer-link interface. |
N/A |
port link-type trunk |
Set the link type of the physical port to trunk. |
N/A |
port trunk permit vlan all |
Assign the port to all VLANs. |
N/A |
undo mac-address static source-check enable |
Disable the static source check feature. |
This configuration avoids cross-peer link Layer 3 traffic forwarding failure. This configuration is not required for S12500X-AF/S12500G-AF/S12500R/S6890, because such an issue will not occur on the device. |
quit |
quit |
N/A |
N/A |
vlan 4094 |
vlan 4094 |
Create VLAN 4094. |
N/A |
quit |
quit |
N/A |
N/A |
interface Vlan-interface 4094 |
Create VLAN-interface 4094. |
N/A |
ip address 100.100.100.1 255.255.255.252 |
ip address 100.100.100.2 255.255.255.252 |
Assign an IP address to the interface for establishing IBGP peer connection on the peer link. |
N/A |
quit |
quit |
N/A |
N/A |
interface Bridge-Aggregation 1 |
Enter the view of Bridge-Aggregation 1. |
N/A |
Configure Bridge-Aggregation 1 to operate in dynamic mode, and enable LACP. |
N/A |
lacp edge-port |
lacp edge-port |
Configure the aggregate interface as an edge aggregate interface. |
N/A |
port m-lag group 1 |
Assign the aggregate interface to an M-LAG group. |
N/A |
quit |
quit |
N/A |
N/A |
ip vpn-instance m-lag-keepalive |
Create VPN instance m-lag-keepalive. |
N/A |
route-distinguisher 100:1 |
Configure the RD of the VPN instance. |
N/A |
vpn-target 1:1 |
vpn-target 1:1 |
Configure the RT of the VPN instance. |
N/A |
quit |
quit |
N/A |
N/A |
interface Twenty-FiveGigE1/0/2 |
Enter the view of interface Twenty-FiveGigE 1/0/2. |
N/A |
port link-mode route |
Configure the Ethernet interface to work in Layer 3 mode. |
N/A |
ip binding vpn-instance m-lag-keepalive |
Associate the interface with VPN instance m-lag-keepalive. |
N/A |
ip address 100.100.100.5 255.255.255.252 |
ip address 100.100.100.6 255.255.255.252 |
Configure the IP address for the keepalive link. |
N/A |
quit |
quit |
N/A |
N/A |
m-lag role priority 10000 |
m-lag role priority 40000 |
Set the M-LAG role priority of the device. |
N/A |
m-lag system-mac 8465-6958-e2c4 |
Configure the M-LAG system MAC address. |
N/A |
m-lag system-number 1 |
m-lag system-number 2 |
Set the M-LAG system number. |
N/A |
m-lag system-priority 10000 |
Set the M-LAG system priority. |
N/A |
m-lag standalone enable |
Enable M-LAG standalone mode. |
N/A |
m-lag keepalive ip destination 100.100.100.6 source 100.100.100.5 vpn-instance m-lag-keepalive |
m-lag keepalive ip destination 100.100.100.5 source 100.100.100.6 vpn-instance m-lag-keepalive |
Configure M-LAG keepalive packet parameters. |
N/A |
m-lag mad exclude interface Twenty-FiveGigE1/0/2 |
Configure M-LAG MAD to not shut down the interface attached to the keepalive link. |
N/A |
m-lag mad exclude interface Vlan-interface 4094 |
Configure M-LAG MAD to not shut down the Layer 3 interconnection interface for fast entry synchronization upon recovery of the M-LAG interface from a failure. |
N/A |
m-lag restore-delay 300 |
Set the data restoration interval for more data synchronization time and faster convergence. |
N/A |
stp instance 0 root primary |
Configure the M-LAG member device as the root bridge. |
N/A |
stp global enable |
stp global enable |
Enable the spanning tree feature globally. |
N/A |
stp tc-protection |
stp tc-protection |
Enable TC-BPDU attack guard for the device to avoid frequent deletion of MAC address entries and ARP entries. |
N/A |
stp bpdu-protection |
Enable BPDU guard globally. |
N/A |
M-LAG 1 |
M-LAG 2 |
Remarks |
vlan 100 |
vlan 100 |
Configure the VLAN used to communicate with a virtualization server. |
N/A |
quit |
quit |
N/A |
N/A |
interface Vlan-interface 100 |
Create VLAN-interface 100. |
N/A |
ip address 10.40.196.61 255.255.255.192 ip address 100.127.128.253 255.255.255.0 sub |
ip address 10.40.196.62 255.255.255.192 ip address 100.127.128.254 255.255.255.0 sub |
Assign the primary and secondary IP addresses to VLAN-interface 100. |
N/A |
vrrp vrid 1 virtual-ip 10.40.196.1 |
Configure the virtual IP address of a VRRP group. |
N/A |
vrrp vrid 1 priority 200 |
vrrp vrid 1 priority 100 |
Configure the priority of the device in the VRRP group. |
VRRP determines the role (master or backup) of each router in a VRRP group by priority. A router with higher priority is more likely to become the master. |
quit |
quit |
N/A |
N/A |
m-lag mad exclude interface Vlan-interface 100 |
Configure M-LAG MAD to not shut down the interface connected to the server for fast entry synchronization upon recovery of the M-LAG interface from a failure. |
As a best practice, do not configure this command for an S12500G-AF device. If you configure this command for the device, the fault recovery time might exceed 500 milliseconds. |
M-LAG 2 |
Remarks |
vlan 2 to 1000 |
vlan 2 to 1000 |
Create VLANs. |
N/A |
quit |
quit |
N/A |
N/A |
interface Twenty-FiveGigE1/0/1 |
Configuring the interface used to connect to the Layer 3 virtualization server. |
N/A |
port link-aggregation group 1 |
Assign the physical port to Layer 2 aggregation group 1. |
N/A |
quit |
quit |
N/A |
N/A |
N/A |
N/A |
port trunk permit vlan 2 to 1000 |
Assign the port to VLAN 2 through VLAN 1000. |
N/A |
port trunk pvid vlan 100 |
Set the PVID for the trunk port to 100. |
N/A |
quit |
quit |
N/A |
N/A |
M-LAG 2 |
Remarks |
interface HundredGigE1/0/27 |
interface HundredGigE1/0/28 |
Enter view of the interface connected to Core 2. |
N/A |
N/A |
ip address 10.39.245.13 255.255.255.254 |
ip address 10.39.245.45 255.255.255.254 |
Assign an IP address to the interface. |
N/A |
quit |
quit |
N/A |
N/A |
Enter view of the interface connected to Core 1. |
N/A |
N/A |
ip address 10.39.244.13 255.255.255.254 |
ip address 10.39.244.45 255.255.255.254 |
N/A |
quit |
quit |
N/A |
N/A |
M-LAG 2 |
Remarks |
bgp 65115 |
bgp 65115 |
Enable the specified BGP instance and enter its view. |
N/A |
bgp update-delay on-startup 120 |
Configure BGP to delay sending route updates on reboot, and set the delay timer to 120 seconds. |
The M-LAG member devices learn route entries after synchronizing MAC address entries and ARP entries. |
non-stop-routing |
non-stop-routing |
Enable BGP nonstop routing (NSR). |
Avoid forwarding interruption on the M-LAG member devices. |
router-id 10.41.254.140 |
router-id 10.41.254.141 |
Specify the router ID for the BGP instance. |
N/A |
group M-LAG internal |
Create an IBGP peer group named M-LAG. |
N/A |
peer M-LAG route-update-interval 0 |
Specify the interval for sending the same update to the peer group as 0. |
Enable the device to fast send update to the peer group upon route changes to speed up route convergence after an M-LAG primary/secondary switchover occurs. |
peer M-LAG timer keepalive 10 hold 30 |
Set the keepalive interval and hold time for the peer group to 10 seconds and 30 seconds, respectively. |
N/A |
group core external |
Create an EBGP peer group to connect to the core device. |
N/A |
peer core as-number 65105 |
Configure the AS number of the EBGP peer group. |
N/A |
peer core route-update-interval 0 |
peer core timer keepalive 10 hold 30 |
N/A |
peer 10.39.244.12 group core |
peer 10.39.244.44 group core |
Add Core 1 as a peer to peer group core. |
N/A |
peer 10.39.245.12 group core |
peer 10.39.245.44 group core |
Add Core 2 as a peer to peer group core. |
N/A |
peer 100.100.100.2 group M-LAG |
peer 100.100.100.1 group M-LAG |
Add the other M-LAG as a peer to peer group M-LAG. |
N/A |
address-family ipv4 unicast |
Enter BGP IPv4 unicast address family view. |
N/A |
balance 8 |
balance 8 |
Enable load balancing and set the maximum number of BGP ECMP routes as 8 for load balancing. |
N/A |
preference 180 200 130 |
Set preferences for EBGP, IBGP, and local routes to 180, 200, and 130, respectively. |
Adjust the possibility of selecting BGP routes as optimal routes. |
import-route direct |
Redistribute direct routes. |
N/A |
import-route ospf |
import-route ospf |
Redistribute OSPF routes between the M-LAG member device and server. |
N/A |
peer core enable |
peer core enable |
Enable BGP to exchange routing information with peer group core. |
N/A |
peer core advertise-community |
Advertise the COMMUNITY attribute to peer group core. |
N/A |
peer M-LAG enable |
peer M-LAG enable |
Enable BGP to exchange routing information with peer group M-LAG. |
N/A |
peer M-LAG next-hop-local |
Set the local router as the next hop for routes sent to peer group M-LAG. |
N/A |
Perform this task or the task in "Configuring OSPF between the M-LAG member devices and the server."
M-LAG 2 |
Remarks |
bgp 65115 |
bgp 65115 |
Use BGP to implement Layer 3 connectivity between the M-LAG member devices and the server. |
group docker_host external |
Create an EBGP peer group to connect to the server. |
N/A |
peer docker_host as-number 60000 |
N/A |
peer 100.127.128.3 group docker_host |
Add the server (with IP address 100.127.128.3) to peer group docker_host. |
N/A |
N/A |
peer docker_host enable |
Enable BGP to exchange routing information with peer group docker_host. |
Establish EBGP peer with the Layer 3 virtualization server. |
peer docker_host route-limit 5000 |
Set the maximum number of routes that can be received from a peer group. |
N/A |
Perform this task or the task in "Configuring BGP between the M-LAG member devices and the server."
M-LAG 1 |
M-LAG 2 |
Remarks |
ospf 1 |
ospf 1 |
Enable OSPF and enter OSPF view. |
Use OSPF to implement Layer 3 connectivity between the M-LAG member devices and the server. |
stub-router include-stub on-startup 900 |
Specify the cost of the stub links (link type 3) in Router LSAs to the maximum value 65535, in order to speed up convergence. |
N/A |
Redistribute direct routes into the OSPF routing table. |
N/A |
import-route bgp |
import-route bgp |
Redistribute BGP routes into the OSPF routing table. |
N/A |
area 0.0.0.0 |
area 0.0.0.0 |
Enter OSPF area view. |
N/A |
network 100.127.128.0 0.0.0.255 |
Configure OSPF to advertise the local network route. |
N/A |
quit |
quit |
Exit OSPF area view. |
N/A |
Core 2 |
Remarks |
interface HundredGigE1/0/1 |
interface HundredGigE1/0/2 |
Enter the view of the interface connected to M-LAG 1. |
N/A |
Configure the interface to work in Layer 3 mode. |
N/A |
ip address 10.39.244.12 255.255.255.254 |
ip address 10.39.245.12 255.255.255.254 |
N/A |
quit |
quit |
N/A |
N/A |
Enter the view of the interface connected to M-LAG 2. |
N/A |
N/A |
ip address 10.39.244.44 255.255.255.254 |
ip address 10.39.245.44 255.255.255.254 |
N/A |
quit |
quit |
N/A |
N/A |
Core 2 |
Remarks |
interface HundredGigE1/0/3 |
Enter the view of the interface connected to the service network. |
N/A |
N/A |
ip address 22.22.1.1 255.255.255.0 |
ip address 12.12.1.1 255.255.255.0 |
N/A |
quit |
quit |
Exit interface view. |
N/A |
Core 2 |
Remarks |
bgp 65105 |
bgp 65105 |
N/A |
group M-LAG external |
Create an EBGP peer group named M-LAG. |
N/A |
peer M-LAG as-number 65115 |
Specify an AS number for EBGP peer group M-LAG. |
N/A |
peer 10.39.244.45 group M-LAG |
peer 10.39.245.45 group M-LAG |
Add M-LAG2 as a peer to peer group M-LAG. |
N/A |
peer 10.39.244.13 group M-LAG |
peer 10.39.245.13 group M-LAG |
Add M-LAG1 as a peer to peer group M-LAG. |
N/A |
N/A |
balance 8 |
balance 8 |
Enable load balancing and set the maximum number of BGP ECMP routes for load balancing. |
N/A |
N/A |
Redistribute direct routes into the BGP routing table. |
N/A |
import-route ospf |
import-route ospf |
Redistribute OSPF routes into the BGP routing table. |
N/A |
peer M-LAG enable |
peer M-LAG enable |
N/A |
peer M-LAG preferred-value 60000 |
Set preferred value 60000 for routes received from peer group M-LAG. |
Enable the routes received from the peer group to become the optimal routes. |
quit |
quit |
Exit BGP view. |
N/A |
Core 2 |
Remarks |
ospf 1 |
ospf 1 |
N/A |
N/A |
N/A |
import-route bgp |
import-route bgp |
N/A |
area 0.0.0.0 |
area 0.0.0.0 |
N/A |
network 22.22.1.0 0.0.0.255 |
network 12.12.1.0 0.0.0.255 |
Configure OSPF to advertise the service network route. |
N/A |
quit |
quit |
N/A |
Traffic forwarding models
Traffic type: Known IPv4 unicast, Layer 2 unicast, and unknown unicast.
Direction: South to north, north to south, east to west across the M-LAG system, and west to east across the M-LAG system.
Forwarding path: Server > M-LAG system > core devices > service network, service network > core devices > M-LAG system > server, M-LAG 2 > M-LAG 1, and M-LAG 1 > M-LAG 2.
Traffic simulation: Send packets by using the tester.
Load: Light load (less than 1000 flows).
Traffic direction to firewalls/LB: N/A
Traffic type |
Direction |
Forwarding path |
Traffic simulation |
Load |
Traffic direction to firewalls/LB |
Remarks |
Known IPv4 unicast |
South to north |
Server > M-LAG system > core devices > service network |
Tester |
Light |
N/A |
N/A |
North to south |
Service network > core devices > M-LAG system > server |
Tester |
Light |
N/A |
N/A |
East to west across the M-LAG system |
M-LAG 2 > M-LAG 1 |
Tester |
Light |
N/A |
N/A |
West to east across the M-LAG system |
M-LAG 1 > M-LAG 2 |
Tester |
Light |
N/A |
N/A |
Layer 2 unicast |
South to north |
Server > M-LAG system |
Tester |
Light |
N/A |
N/A |
Layer 2 unicast |
North to south |
Tester |
Light |
N/A |
N/A |
Layer 2 unicast |
M-LAG 2 > M-LAG 1 |
Tester |
Light |
N/A |
N/A |
Layer 2 unicast |
M-LAG 1 > M-LAG 2 |
Tester |
Light |
N/A |
N/A |
Unknown unicast |
South to north |
Tester |
Light |
N/A |
N/A |
Unknown unicast |
North to south |
Tester |
Light |
N/A |
N/A |
Unknown unicast |
M-LAG 2 > M-LAG 1 |
Tester |
Light |
N/A |
N/A |
Unknown unicast |
M-LAG 1 > M-LAG 2 |
Tester |
Light |
N/A |
N/A |
Verification commands
M-LAG 1 |
M-LAG 2 |
display m-lag summary |
Displays summary information about M-LAG interfaces. |
display m-lag system |
Displays the M-LAG system settings. |
display m-lag keepalive |
Displays M-LAG keepalive packet statistics. |
display m-lag role |
Displays M-LAG role information. |
display m-lag consistency { type1 | type2 } |
Displays information about the configuration consistency check done by M-LAG. |
display m-lag consistency-check status |
Displays the configuration consistency check status. |
display interface Bridge-Aggregation [ brief ] |
Displays information about aggregate interfaces. |
# Display the M-LAG system settings on M-LAG 1 to verify that M-LAG 1 and M-LAG 2 has established an M-LAG system.
[M-LAG1] display m-lag system
System information
Local system number: 1 Peer system number: 2
Local system MAC: 8465-6958-e2c4 Peer system MAC: 8465-6958-e2c4
Local system priority: 10000 Peer system priority: 10000
Local bridge MAC: 0068-5116-5101 Peer bridge MAC: 90e7-1062-5371
Local effective role: Primary Peer effective role: Secondary
Health level: 0
Standalone mode on split: Enabled
In standalone mode: No
System timer information
Timer State Value (s) Remaining time (s)
Auto recovery Disabled - -
Restore delay Disabled 300 -
Consistency-check delay Disabled 150 -
Standalone delay Disabled - -
Role to None delay Disabled 60 -
# View summary information about M-LAG interfaces on M-LAG 1.
[M-LAG1] display m-lag summary
Flags: A -- Aggregate interface down, B -- No peer M-LAG interface configured
C -- Configuration consistency check failed
Peer-link interface: BAGG1024
Peer-link interface state (cause): UP
Keepalive link state (cause): UP
M-LAG interface information
M-LAG IF M-LAG group Local state (cause) Peer state Remaining down time(s)
BAGG1 1 UP UP -
# View M-LAG role information on M-LAG 1.
[M-LAG1] display m-lag role
Effective role information
Factors Local Peer
Effective role Primary Secondary
Initial role Primary Secondary
MAD DOWN state No Yes
Health level 0 0
Role priority 10000 40000
Bridge MAC 0068-5116-5101 90e7-1062-5371
Effective role trigger: Peer link calculation
Effective role reason: MAD status
Configured role information
Factors Local Peer
Configured role Primary Secondary
# View information about the aggregate interfaces on M-LAG 1.
[M-LAG1] display interface Bridge-Aggregation brief
Speed: (a) - auto
Interface Link Speed Duplex Type PVID Description
BAGG1 UP 25G(a) F(a) T 100
BAGG1024 UP 200G(a) F(a) T 1
Table 1 Network convergence upon single points of failure
Device |
Failure type |
Traffic interruption time |
M-LAG member device |
Link failure. |
≤ 500 ms |
Node failure. |
Fixed-port device: < 500 ms Modular device: · Device replacement: < 1000 ms · Switching fabric module replacement: 0 ms · Service module replacement: < 500 ms |
Upgrading the devices
Upgrading the M-LAG member devices
Checking the environment
Execute the commands in "Verification commands" and the following commands to verify that the device is available for an upgrade.
M-LAG 1 |
M-LAG 2 |
display device |
display device |
Displays device information. |
display boot-loader |
Displays current software images and startup software images. |
display version |
display version |
Displays system version information. |
See H3C Switches M-LAG System Upgrade & Replacement & Expansion Guide.
Verifying the traffic interruption time during the upgrade
Verify that the traffic interruption time is shorter than 500 ms during a switchover and shorter than 150 ms during fallback. For more information, see "Testing network convergence."
Verifying the upgrade result
Execute the commands in "Verification commands" and the following commands to verify that the device is upgraded successfully.
M-LAG 1 |
M-LAG 2 |
display device |
display device |
display version |
display version |
Expanding the network
An expansion operation adds two leaf devices.
Expanding the M-LAG system
Execute the commands in "Verification commands" and the following commands to verify that the device is available for an expansion.
M-LAG 1 |
M-LAG 2 |
display device |
display device |
display version |
display version |
Adding the device to the M-LAG system
1. Disconnect the device from network management systems.
2. Upgrade the software of the device as needed.
3. Preconfigure the device.
4. Connect the device to network management systems.
5. Incorporate the device on the controller.
Verifying the expansion result
Execute the following commands to verify that the device is added successfully.
M-LAG 1 |
M-LAG 2 |
display device |
display device |
display version |
display version |
Replacing hardware
Replacing a service module
Execute the commands in "Verification commands" and the following commands to verify that the target device is available for a replacement.
M-LAG 1 |
M-LAG 2 |
display device |
display device |
display version |
display version |
1. Switch service and management traffic on the target service module to other service modules.
2. Power off the device and replace the service module, or replace the service module when the device is running. For more information, see the installation guides for the service module.
For details, see H3C Switches M-LAG System Upgrade & Replacement & Expansion Guide.
Verifying the replacement result
Execute the commands in "Checking the environment."
Replacing a switching fabric module
M-LAG 1 |
M-LAG 2 |
display device |
display device |
display version |
display version |
Power off the device and replace the switching fabric module, or replace the switching fabric module when the device is running. For more information, see the installation guides for the switching fabric module.