11-Network Management and Monitoring Configuration Guide
HomeSupportSwitchesS6520X-EI SeriesConfigure & DeployConfiguration GuidesH3C S6520X & S6520-SI & S5560X-HI & S5000-EI & MS4600 Configuration Guides-R6636Pxx-6W10011-Network Management and Monitoring Configuration Guide
22-Information center configuration
22-Information center configuration 227.44 KB
Configuring the information center 1
About the information center 1
Log types· 1
Log levels· 1
Log destinations· 2
Default output rules for logs· 2
Default output rules for diagnostic logs· 2
Default output rules for security logs· 2
Default output rules for hidden logs· 3
Default output rules for trace logs· 3
Log formats and field descriptions· 3
FIPS compliance· 6
Information center tasks at a glance· 6
Managing standard system logs· 6
Managing hidden logs· 7
Managing security logs· 7
Managing diagnostic logs· 7
Managing trace logs· 8
Enabling the information center 8
Outputting logs to various destinations· 8
Outputting logs to the console· 8
Outputting logs to the monitor terminal 9
Outputting logs to log hosts· 10
Outputting logs to the log buffer 11
Saving logs to the log file· 11
Setting the minimum storage period· 12
Enabling synchronous information output 13
Configuring log suppression· 13
Enabling duplicate log suppression· 13
Configuring log suppression for a module· 15
Disabling an interface from generating link up or link down logs· 15
Enabling SNMP notifications for system logs· 16
Managing security logs· 16
Saving security logs to the security log file· 16
Managing the security log file· 17
Saving diagnostic logs to the diagnostic log file· 18
Setting the maximum size of the trace log file· 18
Display and maintenance commands for information center 19
Information center configuration examples· 19
Example: Outputting logs to the console· 19
Example: Outputting logs to a UNIX log host 20
Example: Outputting logs to a Linux log host 21
The information center on the device receives logs generated by source modules and outputs logs to different destinations according to log output rules. Based on the logs, you can monitor device performance and troubleshoot network problems.
Figure 1 Information center diagram
Log types
Logs are classified into the following types:
·     Standard system logs—Record common system information. Unless otherwise specified, the term "logs" in this document refers to standard system logs.
·     Diagnostic logs—Record debugging messages.
·     Security logs—Record security information, such as authentication and authorization information.
·     Hidden logs—Record log information not displayed on the terminal, such as input commands.
·     Trace logs—Record system tracing and debugging messages, which can be viewed only after the devkit package is installed.
Log levels
Logs are classified into eight severity levels from 0 through 7 in descending order. The information center outputs logs with a severity level that is higher than or equal to the specified level. For example, if you specify a severity level of 6 (informational), logs that have a severity level from 0 to 6 are output.
Table 1 Log levels
Severity value
Level
0
Emergency
The system is unusable. For example, the system authorization has expired.
1
Alert
Action must be taken immediately. For example, traffic on an interface exceeds the upper limit.
2
Critical
Critical condition. For example, the device temperature exceeds the upper limit, the power module fails, or the fan tray fails.
3
Error
Error condition. For example, the link state changes.
4
Warning
Warning condition. For example, an interface is disconnected, or the memory resources are used up.
5
Notification
Normal but significant condition. For example, a terminal logs in to the device, or the device reboots.
6
Informational
Informational message. For example, a command or a ping operation is executed.
7
Debugging
Debugging message.
Log destinations
The system outputs logs to the following destinations: console, monitor terminal, log buffer, log host, and log file. Log output destinations are independent and you can configure them after enabling the information center. One log can be sent to multiple destinations.
A log output rule specifies the source modules and severity level of logs that can be output to a destination. Logs matching the output rule are output to the destination. Table 2 shows the default log output rules.
Table 2 Default output rules
Destination
Log source modules
Output switch
Severity
Console
All supported modules
Enabled
Debugging
Monitor terminal
Disabled
Debugging
Log host
Enabled
Informational
Log buffer
Enabled
Informational
Log file
Enabled
Informational
Diagnostic logs can only be output to the diagnostic log file, and cannot be filtered by source modules and severity levels. Table 3 shows the default output rule for diagnostic logs.
Table 3 Default output rule for diagnostic logs
Destination
Log source modules
Output switch
Severity
Diagnostic log file
Enabled
Debugging
Security logs can only be output to the security log file, and cannot be filtered by source modules and severity levels. Table 4 shows the default output rule for security logs.
Table 4 Default output rule for security logs
Destination
Log source modules
Output switch
Severity
Security log file
Disabled
Debugging
Hidden logs can be output to the log host, the log buffer, and the log file. Table 5 shows the default output rules for hidden logs.
Table 5 Default output rules for hidden logs
Destination
Log source modules
Output switch
Severity
Log host
Enabled
Informational
Log buffer
Enabled
Informational
Log file
Enabled
Informational
Trace logs can only be output to the trace log file, and cannot be filtered by source modules and severity levels. Table 6 shows the default output rules for trace logs.
Table 6 Default output rules for trace logs
Destination
Log source modules
Output switch
Severity
Trace log file
Enabled
Debugging
Log formats
The format of logs varies by output destinations. Table 7 shows the original format of log information, which might be different from what you see. The actual format varies by the log resolution tool used.
Table 7 Log formats
Output destination
Format
Console, monitor terminal, log buffer, or log file
Prefix Timestamp Sysname Module/Level/Mnemonic: Content
Example:
%Nov 24 14:21:43:502 2019 Sysname SHELL/5/SHELL_LOGIN: VTY logged in from 192.168.1.26
Log host
Non-customized format:
<PRI>Timestamp Sysname %%vvModule/Level/Mnemonic: Location; Content
Example:
<190>Nov 24 16:22:21 2019 Sysname %%10SHELL/5/SHELL_LOGIN: -DevIP=1.1.1.1; VTY logged in from 192.168.1.26<190>Nov 24 16:22:21 2016 Sysname %%10 SHELL/5/SHELL_LOGIN: -DevIP=1.1.1.1; VTY logged in from 192.168.1.26
CMCC format:
<PRI>Timestamp Sysname %vvModule/Level/Mnemonic: Location; Content
<189>Oct 9 14:59:04 2019 Sysname %10SHELL/5/SHELL_LOGIN: VTY logged in from 192.168.1.21
RFC 5424 format:
<PRI>Version Timestamp Sysname Module - Mnemonic [SysLoc][AppLoc] Content
<190>1 2020-09-25T10:42:22.257Z Sysname SHELL – SHELL_LOGIN [SysLoc@25506 VendorID=%%10 Level=6][AppLoc@25506 Line=vty0 IPAddr=192.168.1.21 User=**] VTY logged in from 192.168.1.21
SGCC format:
<PRI> Timestamp Sysname Devtype Content
<189> 2019-03-18 15:39:45 Sysname FW 0 2 admin 10.1.1.1
Unicom format:
<PRI>Timestamp Hostip vvModule/Level/Serial_number: Content
Example:
<189>Oct 13 16:48:08 2019 10.1.1.1 10SHELL/5/210231a64jx073000020: VTY logged in from 192.168.1.21
Log field description
Table 8 Log field description
Prefix (information type)
A log to a destination other than the log host has an identifier in front of the timestamp:
·     An identifier of percent sign (%) indicates a log with a level equal to or higher than informational.
·     An identifier of asterisk (*) indicates a debugging log or a trace log.
·     An identifier of caret (^) indicates a diagnostic log.
PRI (priority)
A log destined for the log host has a priority identifier in front of the timestamp. The priority is calculated by using this formula: facility*8+level, where:
·     facility is the facility name. Facility names local0 through local7 correspond to values 16 through 23. The facility name can be configured using the info-center loghost command. It is used to identify log sources on the log host, and to query and filter the logs from specific log sources.
·     level is in the range of 0 to 7. See Table 1 for more information about severity levels.
Timestamp
Records the time when the log was generated.
Logs sent to the log host and those sent to the other destinations have different timestamp precisions, and their timestamp formats are configured with different commands. For more information, see Table 9 and Table 10.
Hostip
Source IP address of the log. If the info-center loghost source command is configured, this field displays the IP address of the specified source interface. Otherwise, this field displays the sysname.
This field exists only in logs that are sent to the log host in unicom format.
Serial number
Serial number of the device that generated the log.
Sysname (host name or host IP address)
The sysname is the host name or IP address of the device that generated the log. You can use the sysname command to modify the name of the device.
%% (vendor ID)
Indicates that the information was generated by an H3C device.
This field exists only in logs sent to the log host.
vv (version information)
Identifies the version of the log, and has a value of 10.
This field exists only in logs that are sent to the log host.
Module
Specifies the name of the module that generated the log. You can enter the info-center source ? command in system view to view the module list.
Level
Identifies the level of the log. See Table 1 for more information about severity levels.
Mnemonic
Describes the content of the log. It contains a string of up to 32 characters.
Location
Optional field that identifies the log sender. This field exists only in logs that are sent to the log host in non-customized or CMCC format.
The field contains the following information:
·     Devlp—IP address of the log sender.
·     Slot—Member ID of the IRF member device that sent the log.
SysLoc
Optional field that identifies the system information of the logs. This field exists only in logs that are sent to the log host in RFC 5424 format.
·     SysLoc@—Vendor number of the device that generates logs.
·     VendorID—Vendor ID. Currently, the fixed value is 10.
·     Level—Log level.
AppLoc
Optional field that identifies the module information of the logs. This field exists only in logs that are sent to the log host in RFC 5424 format.
·     AppLoc@—Vendor number of the device that generates logs.
·     Line—User line used by the current user for login.
·     IPAddr—IP address used for user login.
·     User—Username for login.
Content
Provides the content of the log.
Table 9 Timestamp precisions and configuration commands
Item
Destined for the log host
Destined for the console, monitor terminal, log buffer, and log file
Precision
Seconds (default) or milliseconds
Milliseconds
Command used to set the timestamp format
info-center timestamp loghost
Table 10 Description of the timestamp parameters
Timestamp parameters
boot
Time that has elapsed since system startup, in the format of xxx.yyy. xxx represents the higher 32 bits, and yyy represents the lower 32 bits, of milliseconds elapsed.
Logs that are sent to all destinations other than a log host support this parameter.
Example:
%0.109391473 Sysname FTPD/5/FTPD_LOGIN: User ftp (192.168.1.23) has logged in successfully.
0.109391473 is a timestamp in the boot format.
date
Current date and time.
·     For logs output to a log host, the timestamp can be in the format of MMM DD hh:mm:ss YYYY (accurate to seconds) or MMM DD hh:mm:ss.ms YYYY (accurate to milliseconds).
·     For logs output to other destinations, the timestamp is in the format of MMM DD hh:mm:ss:ms YYYY.
All logs support this parameter.
Example:
%May 30 05:36:29:579 2019 Sysname FTPD/5/FTPD_LOGIN: User ftp (192.168.1.23) has logged in successfully.
May 30 05:36:29:579 2019 is a timestamp in the date format in logs sent to the console.
iso
Timestamp format stipulated in ISO 8601, accurate to seconds (default) or milliseconds.
Only logs that are sent to a log host support this parameter.
Example:
<189>2019-05-30T06:42:44 Sysname %%10FTPD/5/FTPD_LOGIN: User ftp (192.168.1.23) has logged in successfully.
2019-05-30T06:42:44 is a timestamp in the iso format accurate to seconds. A timestamp accurate to milliseconds is like 2019-05-30T06:42:44.708.
none
No timestamp is included.
Example:
% Sysname FTPD/5/FTPD_LOGIN: User ftp (192.168.1.23) has logged in successfully.
no-year-date
Current date and time without year or millisecond information, in the format of MMM DD hh:mm:ss.
Example:
<189>May 30 06:44:22 Sysname %%10FTPD/5/FTPD_LOGIN: User ftp (192.168.1.23) has logged in successfully.
May 30 06:44:22 is a timestamp in the no-year-date format.
FIPS compliance
1.     Enabling the information center
2.     Outputting logs to various destinations
¡     Outputting logs to the console
¡     Outputting logs to the monitor terminal
¡     Outputting logs to log hosts
¡     Outputting logs to the log buffer
¡     Saving logs to the log file
3.     (Optional.) Setting the minimum storage period
4.     (Optional.) Enabling synchronous information output
5.     (Optional.) Configuring log suppression
¡     Enabling duplicate log suppression
¡     Configuring log suppression for a module
¡     Disabling an interface from generating link up or link down logs
6.     (Optional.) Enabling SNMP notifications for system logs
4.     (Optional.) Configuring log suppression
2.     (Optional.) Configuring log suppression
3.     Managing security logs
¡     Saving security logs to the security log file
¡     Managing the security log file
3.     Saving diagnostic logs to the diagnostic log file
Managing trace logs
3.     Setting the maximum size of the trace log file
The information center can output logs only after it is enabled.
2.     Enable the information center.
info-center enable
The information center is enabled by default.
The terminal monitor, terminal debugging, and terminal logging commands take effect only for the current connection between the terminal and the device. If a new connection is established, the default is restored.
2.     (Optional.) Configure an output rule for sending logs to the console.
info-center source { module-name | default } console { deny | level severity }
For information about the default output rules, see "Default output rules for logs."
3.     (Optional.) Configure the timestamp format.
The default timestamp format is date.
4.     Return to user view.
5.     Enable log output to the console.
terminal monitor
By default, log output to the console is enabled.
6.     Enable output of debugging messages to the console.
terminal debugging
By default, output of debugging messages to the console is disabled.
This command enables output of debugging-level log messages to the console.
7.     Set the lowest severity level of logs that can be output to the console.
The default setting is 6 (informational).
Monitor terminals refer to terminals that log in to the device through the AUX or VTY line.
2.     (Optional.) Configure an output rule for sending logs to the monitor terminal.
info-center source { module-name | default } monitor { deny | level severity }
5.     Enable log output to the monitor terminal.
terminal monitor
By default, log output to the monitor terminal is disabled.
6.     Enable output of debugging messages to the monitor terminal.
terminal debugging
By default, output of debugging messages to the monitor terminal is disabled.
This command enables output of debugging-level log messages to the monitor terminal.
7.     Set the lowest level of logs that can be output to the monitor terminal.
The device supports using the information center to output logs of a module to designated log hosts.
2.     (Optional.) Configure a log output filter or a log output rule. Choose one option as needed:
¡     Configure a log output filter.
info-center filter filter-name { module-name | default } { deny | level severity }
You can create multiple log output filters. When specifying a log host, you can apply a log output filter to the log host to control log output.
¡     Configure a log output rule for the log host output destination.
info-center source { module-name | default } loghost { deny | level severity }
For information about the default log output rules for the log host output destination, see "Default output rules for logs."
The system chooses the settings to control log output to a log host in the following order:
a.     Log output filter applied to the log host.
b.     Log output rules configured for the log host output destination by using the info-center source command.
c.     Default log output rules (see "Default output rules for logs").
3.     (Optional.) Specify a source IP address for logs sent to log hosts.
By default, the source IP address of logs sent to log hosts is the primary IP address of their outgoing interfaces.
4.     (Optional.) Specify the format in which logs are output to log hosts.
info-center format { cmcc | rfc5424 | unicom }
By default, logs are output to log hosts in non-customized format.
5.     (Optional.) Add the device serial number to the location field of logs sent to log hosts.
info-center loghost locate-info with-sn
By default, the device does not add the device serial number to the location field of logs sent to log hosts.
6.     (Optional.) Configure the timestamp format.
info-center timestamp loghost { date [ with-milliseconds ] | iso [ with-milliseconds | with-timezone ] * | no-year-date | none }
7.     Specify a log host and configure related parameters.
info-center loghost [ vpn-instance vpn-instance-name ] { hostname | ipv4-address | ipv6 ipv6-address } [ port port-number ] [ dscp dscp-value ] [ facility local-number ] [ filter filter-name ]
By default, no log hosts or related parameters are specified.
The value for the port-number argument must be the same as the value configured on the log host. Otherwise, the log host cannot receive logs.
This feature enables log output to the log buffer. You can use the display logbuffer command to display the log buffer information and the buffered logs.
2.     (Optional.) Configure an output rule for sending logs to the log buffer.
info-center source { module-name | default } logbuffer { deny | level severity }
4.     Enable log output to the log buffer.
info-center logbuffer
By default, log output to the log buffer is enabled.
5.     (Optional.) Set the maximum log buffer size.
By default, a maximum of 512 logs can be buffered.
The log file feature enables log output to the log file. The system saves logs from the log file buffer to the log file. After saving logs to the log file, the system clears the log file buffer.
Log saving from the log file buffer to the log file is triggered by the following situations:
·     Periodic saving.
·     A manual immediate saving of buffered logs to the log file.
·     The log file buffer is full.
A log file is automatically created when needed and has a maximum capacity. The log file capacity restrictions are as follows:
·     When no log file space is available, the device stops saving new logs.
When no log file space or storage device space is available, the system will replace the oldest logs with new logs.
TIP
TIP:
·     Clean up the storage space of the device regularly to ensure sufficient storage space for the log file feature.
·     As a best practice, back up the log files regularly to avoid loss of important logs.
2.     (Optional.) Configure an output rule for sending logs to the log file.
info-center source { module-name | default } logfile { deny | level severity }
3.     Enable the log file feature.
info-center logfile enable
By default, the log file feature is enabled.
4.     (Optional.) Set the maximum log file size.
By default, the maximum log file size is 10 MB.
5.     (Optional.) Specify the log file directory.
The default log file directory is flash:/logfile.
This command cannot survive an IRF reboot or a master/subordinate switchover.
6.     Save logs in the log file buffer to the log file. Choose one or both options as needed:
¡     Configure the automatic log file saving interval.
The default log file saving interval is 86400 seconds.
¡     Immediately save logs from the log file buffer to the log file.
logfile save
This command is available in any view.
Use this feature to set the minimum storage period for logs in the log buffer and log file. This feature ensures that logs will not be overwritten by new logs during a set period of time.
By default, when the log buffer or log file is full, new logs will automatically overwrite the oldest logs. After the minimum storage period is set, the system identifies the storage period of a log to determine whether to delete the log. The system current time minus a log's generation time is the log's storage period.
·     If the storage period of a log is shorter than or equal to the minimum storage period, the system does not delete the log. The new log will not be saved.
·     If the storage period of a log is longer than the minimum storage period, the system deletes the log to save the new log.
2.     Set the log minimum storage period for logs.
info-center syslog min-age min-age
By default, the log minimum storage period is not set.
System log output interrupts ongoing configuration operations, obscuring previously entered commands. Synchronous information output shows the obscured commands. It also provides a command prompt in command editing mode, or a [Y/N] string in interaction mode so you can continue your operation from where you were stopped.
2.     Enable synchronous information output.
info-center synchronous
By default, synchronous information output is disabled.
The information center on the device outputs logs generated by service modules. The device identifies logs that have the same module name, level, mnemonic, location, and text as duplicate logs.
In some scenarios, for example, ARP attack or link failure, the service modules will generate a large volume of duplicate logs during a short period of time. Recording and output of consecutive duplicate logs wastes system and network resources. To resolve this issue, you can enable duplicate log suppression.
With this feature enabled, when a service module generates a log, the information center outputs the log and starts the duplicate log suppression timer. The suppression period of the duplicate log suppression timer varies by phase. The suppression periods in phase 1, 2, and later phases are 30 seconds, 2 minutes, and 10 minutes, respectively.
After you enable duplicate log suppression, the system starts suppression upon outputting a log:
·     If only duplicate logs of the log are received during the suppression period of a phase, the information center does not output the duplicate logs. When the suppression period of the phase expires, the information center outputs the suppressed log and the number of times the log is suppressed, and starts the next suppression phase.
·     If a different log is received during the suppression period of a phase, the information center performs the following operations:
¡     Stops suppression on the log, and outputs the suppressed log and the number of times the log is suppressed.
¡     Outputs the different log and starts phase-1 suppression for that log.
·     If no log is received within the suppression period of any phase, the information center deletes the duplicate log suppression timer, stops suppression on the log, and does not output any log.
2.     Enable duplicate log suppression.
info-center logging suppress duplicates
By default, duplicate log suppression is disabled.
The following example uses SHELL_CMD logs to verify the duplicate log suppression feature. After the user executes a command on the device, the information center receives a SHELL_CMD log generated by the shell module, encapsulates the log, and then outputs the log to the log buffer.
1.     Verify the suppression effect in phases 1, 2, 3, and 4 of a log (with suppression period of 30 seconds, 2 minutes, 10 minutes, and 10 minutes):
# In a lab environment, continuously execute the display logbuffer command for 25 minutes.
# View the output logs in the log buffer.
<Sysname> display logbuffer
Log buffer: Enabled
Max buffer size: 1024
Actual buffer size: 512
Dropped messages: 0
Overwritten messages: 0
Current messages: 5
%Jul 20 13:01:20:615 2022 Sysname SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer
%Jul 20 13:01:50:718 2022 Sysname SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer This message repeated 2 times in last 30 seconds.
%Jul 20 13:03:50:732 2022 Sysname SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer This message repeated 5 times in last 2 minutes.
%Jul 20 13:13:50:830 2022 Sysname SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer This message repeated 10 times in last 10 minutes.
%Jul 20 13:23:50:211 2022 Sysname SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer This message repeated 6 times in last 10 minutes.
¡     The information center received the log SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer.
¡     In phase 1, the log was suppressed twice by the information center.
¡     In phase 2, the log was suppressed five times by the information center.
¡     In phase 3, the log was suppressed 10 times by the information center.
¡     In phase 4, the log was suppressed six times by the information center.
2.     Continue to verify how duplicate log suppression works when a different log is received during the suppression period of a log:
# Execute the display logbuffer command three times, and then execute the display interface brief command.
Log buffer: Enabled
Dropped messages: 0
Current messages: 5
%Jul 20 13:24:56:205 2022 Sysname SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer This message repeated 3 times in last 1 minute 6 seconds.
%Jul 20 13:25:41:205 2022 Sysname SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display interface brief.
<Sysname>
¡     The information center stopped suppression for the log SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display logbuffer.
¡     The information center output the log SHELL/6/SHELL_CMD: -Line=con0-IPAddr=**-User=**; Command is display interface brief, and started suppression for it.
This feature suppresses output of logs. You can use this feature to filter out the logs that you are not concerned with.
Perform this task to configure a log suppression rule to suppress output of all logs or logs with a specific mnemonic value for a module.
2.     Configure a log suppression rule for a module.
By default, the device does not suppress output of any logs from any modules.
By default, an interface generates link up or link down log information when the interface state changes. In some cases, you might want to disable certain interfaces from generating this information. For example:
·     You are concerned about the states of only some interfaces. In this case, you can use this function to disable other interfaces from generating link up and link down log information.
·     An interface is unstable and continuously outputs log information. In this case, you can disable the interface from generating link up and link down log information.
Use the default setting in normal cases to avoid affecting interface status monitoring.
2.     Enter interface view.
3.     Disable the interface from generating link up or link down logs.
undo enable log updown
By default, an interface generates link up and link down logs when the interface state changes.
This feature enables the device to send an SNMP notification for each log message it outputs. The device encapsulates the logs in SNMP notifications and then sends them to the SNMP module and the log trap buffer.
You can configure the SNMP module to send received SNMP notifications in SNMP traps or informs to remote hosts. For more information, see "Configuring SNMP."
To view the traps in the log trap buffer, access the MIB corresponding to the log trap buffer.
2.     Enable SNMP notifications for system logs.
snmp-agent trap enable syslog
By default, the device does not send SNMP notifications for system logs.
3.     Set the maximum number of traps that can be stored in the log trap buffer.
By default, the log trap buffer can store a maximum of 1024 traps.
Security logs are very important for locating and troubleshooting network problems. Generally, security logs are output together with other logs. It is difficult to identify security logs among all logs.
To solve this problem, you can save security logs to the security log file without affecting the current log output rules.
After you enable the security log file feature, the system processes security logs as follows:
1.     Outputs security logs to the security log file buffer.
2.     Saves logs from the security log file buffer to the security log file at the specified interval.
If you have the security-audit role, you can also manually save security logs to the security log file.
3.     Clears the security log file buffer immediately after the security logs are saved to the security log file.
The device supports only one security log file. The system will overwrite old logs with new logs when the security log file is full. To avoid security log loss, you can set an alarm threshold for the security log file usage ratio. When the alarm threshold is reached, the system outputs a message to inform you of the alarm. You can log in to the device with the security-audit user role and back up the security log file to prevent the loss of important data.
2.     Enable the security log file feature.
info-center security-logfile enable
By default, the security log file feature is disabled.
3.     Set the interval at which the system saves security logs.
The default security log file saving interval is 86400 seconds.
4.     (Optional.) Set the maximum size for the security log file.
By default, the maximum security log file size is 10 MB.
5.     (Optional.) Set the alarm threshold of the security log file usage.
By default, the alarm threshold of the security log file usage ratio is 80. When the usage of the security log file reaches 80%, the system will send a message.
To use the security log file management commands, you must have the security-audit user role. For information about configuring the security-audit user role, see AAA in Security Configuration Guide.
2.     Change the directory of the security log file.
By default, the security log file is saved in the seclog directory in the root directory of the storage device.
The device uses the default security log file directory after an IRF reboot or a master/subordinate switchover.
3.     Manually save all logs in the security log file buffer to the security log file.
security-logfile save
4.     (Optional.) Display the summary of the security log file.
display security-logfile summary
By default, the diagnostic log file feature saves diagnostic logs from the diagnostic log file buffer to the diagnostic log file at the specified saving interval. You can also manually trigger an immediate saving of diagnostic logs to the diagnostic log file. After saving diagnostic logs to the diagnostic log file, the system clears the diagnostic log file buffer.
The device supports only one diagnostic log file. The diagnostic log file has a maximum capacity. When the capacity is reached, the system replaces the oldest diagnostic logs with new logs.
2.     Enable the diagnostic log file feature.
info-center diagnostic-logfile enable
By default, the diagnostic log file feature is enabled.
3.     (Optional.) Set the maximum diagnostic log file size.
By default, the maximum diagnostic log file size is 10 MB.
4.     (Optional.) Specify the diagnostic log file directory.
The default diagnostic log file directory is flash:/diagfile.
The device uses the default diagnostic log file directory after an IRF reboot or a master/subordinate switchover.
5.     Save diagnostic logs in the diagnostic log file buffer to the diagnostic log file. Choose one option as needed:
¡     Configure the automatic diagnostic log file saving interval.
The default saving interval is 86400 seconds.
¡     Manually save diagnostic logs to the diagnostic log file.
diagnostic-logfile save
The device has only one trace log file. When the trace log file is full, the device overwrites the oldest trace logs with new ones.
2.     Set the maximum size for the trace log file.
The default maximum size of the trace log file is 1 MB.
Display the diagnostic log file configuration.
display diagnostic-logfile summary
Display the information center configuration.
display info-center
Display information about log output filters.
display info-center filter [ filter-name ]
Display log buffer information and buffered logs.
display logbuffer  [ reverse ] [ level severity | size buffersize | slot slot-number ] * [ last-mins mins ]
Display the log buffer summary.
display logbuffer summary [ level severity | slot slot-number ] *
Display the content of the log file buffer.
display logfile buffer
Display the log file configuration.
display logfile summary
Display the content of the security log file buffer. (To execute this command, you must have the security-audit user role.)
display security-logfile buffer
Display summary information of the security log file.
Clear the log buffer.
reset logbuffer
Configure the device to output to the console FTP logs that have a minimum severity level of warning.
Figure 2 Network diagram
# Enable the information center.
[Device] info-center enable
# Disable log output to the console.
[Device] info-center source default console deny
To avoid output of unnecessary information, disable all modules from outputting log information to the specified destination (console in this example) before you configure the output rule.
# Configure an output rule to output to the console FTP logs that have a minimum severity level of warning.
[Device] info-center source ftp console level warning
[Device] quit
# Enable log output to the console.
<Device> terminal logging level 6
<Device> terminal monitor
Now, if the FTP module generates logs, the information center automatically sends the logs to the console, and the console displays the logs.
Configure the device to output to the UNIX log host FTP logs that have a minimum severity level of informational.
Figure 3 Network diagram
1.     Make sure the device and the log host can reach each other. (Details not shown.)
2.     Configure the device:
# Specify log host 1.2.0.1/16 with local4 as the logging facility.
[Device] info-center loghost 1.2.0.1 facility local4
# Disable log output to the log host.
To avoid output of unnecessary information, disable all modules from outputting logs to the specified destination (loghost in this example) before you configure an output rule.
# Configure an output rule to output to the log host FTP logs that have a minimum severity level of informational.
[Device] info-center source ftp loghost level informational
3.     Configure the log host:
The log host configuration procedure varies by the vendor of the UNIX operating system. The following shows an example:
a.     Log in to the log host as a root user.
b.     Create a subdirectory named Device in directory /var/log/, and then create file info.log in the Device directory to save logs from the device.
# mkdir /var/log/Device
c.     Edit file syslog.conf in directory /etc/ and add the following contents:
In this configuration, local4 is the name of the logging facility that the log host uses to receive logs. The value info indicates the informational severity level. The UNIX system records the log information that has a minimum severity level of informational to file /var/log/Device/info.log.
Follow these guidelines while editing file /etc/syslog.conf:
·     Comments must be on a separate line and must begin with a pound sign (#).
·     No redundant spaces are allowed after the file name.
·     The logging facility name and the severity level specified in the /etc/syslog.conf file must be identical to those configured on the device by using the info-center loghost and info-center source commands. Otherwise, the log information might not be output to the log host correctly.
d.     Display the process ID of syslogd, kill the syslogd process, and then restart syslogd by using the –r option to validate the configuration.
# ps -ae | grep syslogd
147
# kill -HUP 147
# syslogd -r &
Now, the device can output FTP logs to the log host, which stores the logs to the specified file.
Configure the device to output to the Linux log host 1.2.0.1/16 FTP logs that have a minimum severity level of informational.
Figure 4 Network diagram
# Specify log host 1.2.0.1/16 with local5 as the logging facility.
[Device] info-center loghost 1.2.0.1 facility local5
To avoid outputting unnecessary information, disable all modules from outputting log information to the specified destination (loghost in this example) before you configure an output rule.
# Configure an output rule to enable output to the log host FTP logs that have a minimum severity level of informational.
The log host configuration procedure varies by the vendor of the Linux operating system. The following shows an example:
b.     Create a subdirectory named Device in directory /var/log/, and create file info.log in the Device directory to save logs from the device.
local5.info /var/log/Device/info.log
In this configuration, local5 is the name of the logging facility that the log host uses to receive logs. The value info indicates the informational severity level. The Linux system will store the log information with a severity level equal to or higher than informational to file /var/log/Device/info.log.
d.     Display the process ID of syslogd, kill the syslogd process, and then restart syslogd by using the -r option to validate the configuration.
Make sure the syslogd process is started with the -r option on the Linux log host.
147
# kill -9 147
# syslogd -r &