- 14-Network Management and Monitoring Configuration Guide
- 02-NQA configuration
- 03-iNQA configuration
- 04-iFIT configuration
- 05-SRPM configuration
- 06-NTP configuration
- 07-PTP configuration
- 08-Network synchronization configuration
- 09-SNMP configuration
- 10-RMON configuration
- 11-NETCONF configuration
- 12-CWMP configuration
- 13-EAA configuration
- 14-Process monitoring and maintenance configuration
- 15-Sampler configuration
- 16-Mirroring configuration
- 17-NetStream configuration
- 18-IPv6 NetStream configuration
- 19-TCP connection trace configuration
- 20-Performance management configuration
- 21-Fast log output configuration
- 22-Flow log configuration
- 23-Information center configuration
- 24-Packet capture configuration
- 25-Flow monitor configuration
| 12-CWMP configuration | 247.54 KB |
Restrictions and guidelines: CWMP configuration
Configuring the preferred ACS attributes
Configuring the default ACS attributes from the CLI
Specifying an SSL client policy for HTTPS connection to ACS
Configuring ACS authentication parameters
Configuring the provision code
Configuring the CWMP connection interface
Configuring autoconnect parameters
Enabling NAT traversal for the CPE
Display and maintenance commands for CWMP
Configuring CWMP
About CWMP
CPE WAN Management Protocol (CWMP), also called "TR-069," is a DSL Forum technical specification for remote management of network devices.
The protocol was initially designed to provide remote autoconfiguration through a server for large numbers of dispersed end-user devices in a network. CWMP can be used on different types of networks, including Ethernet.
CWMP network framework
Figure 1 shows a basic CWMP network framework.
Figure 1 CWMP network framework
A basic CWMP network includes the following network elements:
· ACS—Autoconfiguration server, the management device in the network.
· CPE—Customer premises equipment, the managed device in the network.
· DNS server—Domain name system server. CWMP defines that the ACS and the CPE use URLs to identify and access each other. DNS is used to resolve the URLs.
· DHCP server—Assigns ACS attributes along with IP addresses to CPEs when the CPEs are powered on. DHCP server is optional in CWMP. With a DHCP server, you do not need to configure ACS attributes manually on each CPE. The CPEs can contact the ACS automatically when they are powered on for the first time.
The device is operating as a CPE in the CWMP framework.
Basic CWMP functions
You can autoconfigure and upgrade CPEs in bulk from the ACS.
Autoconfiguration
You can create configuration files for different categories of CPEs on the ACS. Based on the device models and serial numbers of the CPEs, the ACS verifies the categories of the CPEs and issues the associated configuration to them.
The following are methods available for the ACS to issue configuration to the CPE:
· Transfers the configuration file to the CPE, and specifies the file as the next-startup configuration file. At a reboot, the CPE starts up with the ACS-specified configuration file.
· Runs the configuration in the CPE's RAM. The configuration takes effect immediately on the CPE. For the running configuration to survive a reboot, you must save the configuration on the CPE.
CPE software management
The ACS can manage CPE software upgrade.
When the ACS finds a software version update, the ACS notifies the CPE to download the software image file from a specific location. The location can be the URL of the ACS or an independent file server.
If the CPE successfully downloads the software image file and the file is validated, the CPE notifies the ACS of a successful download. If the CPE fails to download the software image file or the file is invalidated, the CPE notifies the ACS of an unsuccessful download.
Data backup
The ACS can require the CPE to upload a configuration file or log file to a specific location. The destination location can be the ACS or a file server.
CPE status and performance monitoring
The ACS can monitor the status and performance of CPEs. Table 1 shows the available CPE status and performance objects for the ACS to monitor.
Table 1 CPE status and performance objects available for the ACS to monitor
Category |
Objects |
Remarks |
Device information |
Manufacturer ManufacturerOUI SerialNumber HardwareVersion SoftwareVersion |
N/A |
Operating status and information |
DeviceStatus UpTime |
N/A |
Configuration file |
ConfigFile |
Local configuration file stored on CPE for upgrade. The ACS can issue configuration to the CPE by transferring a configuration file to the CPE or running the configuration in CPE's RAM. |
CWMP settings |
ACS URL |
URL address of the ACS to which the CPE initiates a CWMP connection. This object is also used for main/backup ACS switchover. |
ACS username ACS password |
When the username and password of the ACS are changed, the ACS changes the ACS username and password on the CPE to the new username and password. When a main/backup ACS switchover occurs, the main ACS also changes the ACS username and password to the backup ACS username and password. |
PeriodicInformEnable |
Whether to enable or disable the periodic Inform feature. |
PeriodicInformInterval |
Interval for periodic connection from the CPE to the ACS for configuration and software update. |
PeriodicInformTime |
Scheduled time for connection from the CPE to the ACS for configuration and software update. |
ConnectionRequestURL (CPE URL) |
N/A |
ConnectionRequestUsername (CPE username) ConnectionRequestPassword (CPE password) |
CPE username and password for authentication from the ACS to the CPE. |
How CWMP works
RPC methods
CWMP uses remote procedure call (RPC) methods for bidirectional communication between CPE and ACS. The RPC methods are encapsulated in HTTP or HTTPS.
Table 2 shows the primary RPC methods used in CWMP.
RPC method |
Get |
The ACS obtains the values of parameters on the CPE. |
Set |
The ACS modifies the values of parameters on the CPE. |
Inform |
The CPE sends an Inform message to the ACS for the following purposes: · Initiates a connection to the ACS. · Reports configuration changes to the ACS. · Periodically updates CPE settings to the ACS. |
Download |
The ACS requires the CPE to download a configuration or software image file from a specific URL for software or configuration update. |
Upload |
The ACS requires the CPE to upload a file to a specific URL. |
Reboot |
The ACS reboots the CPE remotely for the CPE to complete an upgrade or recover from an error condition. |
Autoconnect between ACS and CPE
The CPE automatically initiates a connection to the ACS when one of the following events occurs:
· ACS URL change. The CPE initiates a connection request to the new ACS URL.
· CPE startup. The CPE initiates a connection to the ACS after the startup.
· Timeout of the periodic Inform interval. The CPE re-initiates a connection to the ACS at the Inform interval.
· Expiration of the scheduled connection initiation time. The CPE initiates a connection to the ACS at the scheduled time.
CWMP connection establishment
Step 1 through step 5 in Figure 2 show the procedure of establishing a connection between the CPE and the ACS.
1. After obtaining the basic ACS parameters, the CPE initiates a TCP connection to the ACS.
2. If HTTPS is used, the CPE and the ACS initialize SSL for a secure HTTP connection.
3. The CPE sends an Inform message in HTTPS to initiate a CWMP session.
4. After the CPE passes authentication, the ACS returns an Inform response to establish the session.
5. After sending all requests, the CPE sends an empty HTTP post message.
Figure 2 CWMP connection establishment
Main/backup ACS switchover
Typically, two ACSs are used in a CWMP network for consecutive monitoring on CPEs. When the main ACS needs to reboot, it points the CPE to the backup ACS. Step 6 through step 11 in Figure 3 show the procedure of a main/backup ACS switchover.
1. Before the main ACS reboots, it queries the ACS URL set on the CPE.
2. The CPE replies with its ACS URL setting.
3. The main ACS sends a Set request to change the ACS URL on the CPE to the backup ACS URL.
4. After the ACS URL is modified, the CPE sends a response.
5. The main ACS sends an empty HTTP message to notify the CPE that it has no other requests.
6. The CPE closes the connection, and then initiates a new connection to the backup ACS URL.
Figure 3 Main and backup ACS switchover
CWMP is available only in IPv4 networks. If you configure CWMP in an IPv6 network, the feature does not take effect.
You can configure ACS and CPE attributes from the CPE's CLI, the DHCP server, or the ACS. For an attribute, the CLI- and ACS-assigned values have higher priority than the DHCP-assigned value. The CLI- and ACS-assigned values overwrite each other, whichever is assigned later.
This document only describes configuring ACS and CPE attributes from the CLI and DHCP server. For more information about configuring and using the ACS, see ACS documentation.
CWMP tasks at a glance
To configure CWMP, perform the following tasks:
You can also enable CWMP from a DHCP server.
a. Configuring the preferred ACS attributes
b. (Optional.) Configuring the default ACS attributes from the CLI
a. Specifying an SSL client policy for HTTPS connection to ACS
This task is required when the ACS uses HTTPS for secure access.
b. (Optional.) Configuring ACS authentication parameters
c. (Optional.) Configuring the provision code
d. (Optional.) Configuring the CWMP connection interface
e. (Optional.) Configuring autoconnect parameters
f. (Optional.) Setting the close-wait timer
g. (Optional.) Enabling NAT traversal for the CPE
Enabling CWMP from the CLI
The port number for CWMP service is 7547 and cannot be edited by using CLI. To ensure a correct CWMP service, execute the display tcp | include 7547 command before using this feature to see whether the 7547 port is used by other services. If the port is used by another service, execute the command of the service to change its service port.
1. Enter system view.
2. Enter CWMP view.
cwmp
3. Enable CWMP.
cwmp enable
By default, CWMP is disabled.
Configuring ACS attributes
About ACS attributes
You can configure two sets of ACS attributes for the CPE: preferred and default.
· The preferred ACS attributes are configurable from the CPE's CLI, the DHCP server, and ACS.
· The default ACS attributes are configurable only from the CLI.
If the preferred ACS attributes are not configured, the CPE uses the default ACS attributes for connection establishment.
Assigning ACS attributes from the DHCP server
The DHCP server in a CWMP network assigns the following information to CPEs:
· IP addresses for the CPEs.
· DNS server address.
· ACS URL and ACS login authentication information.
This section introduces how to use DHCP option 43 to assign the ACS URL and ACS login authentication username and password. For more information about IP address pool and DNS, see BRAS Services Configuration Guide.
If the DHCP server is an H3C device, you can configure DHCP option 43 by using the option 43 hex 01length URL username password command. For more information about DHCP, Option 43, and the option command, see BRAS Services Configuration Guide.
· length—A hexadecimal number that indicates the total length of the length, URL, username, and password arguments, including the spaces between these arguments. No space is allowed between the 01 keyword and the length value.
· URL—ACS URL.
· username—Username for the CPE to authenticate to the ACS.
· password—Password for the CPE to authenticate to the ACS.
NOTE: The ACS URL, username and password must use the hexadecimal format and be space separated. |
The following example configures the ACS address as https://169.254.76.31:7547, username as 1234, and password as 5678:
[Sysname] ip pool 0
[Sysname-ip-pool-0] option 43 hex 012368747470733A2F2F3136392E3235342E37362E33313A3735343720313233342035363738
Table 3 Hexadecimal forms of the ACS attributes
Attribute |
Attribute value |
Hexadecimal form |
Length |
35 characters |
23 |
ACS URL |
https://169.254.76.31:7547 |
68747470733A2F2F3136392E3235342E37362E33313A3735343720 NOTE: The two ending digits (20) represent the space. |
ACS connect username |
1234 |
3132333420 NOTE: The two ending digits (20) represent the space. |
ACS connect password |
5678 |
35363738 |
Configuring the preferred ACS attributes from the CLI
2. Enter CWMP view.
cwmp
3. Configure the preferred ACS URL.
cwmp acs url url
By default, no preferred ACS URL has been configured.
4. Configure the username for authentication to the preferred ACS URL.
cwmp acs username username
By default, no username has been configured for authentication to the preferred ACS URL.
5. (Optional.) Configure the password for authentication to the preferred ACS URL.
cwmp acs password { cipher | simple } string
By default, no password has been configured for authentication to the preferred ACS URL.
2. Enter CWMP view.
cwmp
3. Configure the default ACS URL.
cwmp acs default url url
By default, no default ACS URL has been configured.
4. Configure the username for authentication to the default ACS URL.
cwmp acs default username username
By default, no username has been configured for authentication to the default ACS URL.
5. (Optional.) Configure the password for authentication to the default ACS URL.
cwmp acs default password { cipher | simple } string
By default, no password has been configured for authentication to the default ACS URL.
Configuring CPE attributes
About CPE attributes
You can configure the following CPE attributes only from the CPE's CLI.
· CWMP connection interface.
· NAT traversal.
· Maximum number of connection retries.
· SSL client policy for HTTPS connection to ACS.
For other CPE attribute values, you can assign them to the CPE from the CPE's CLI or the ACS. The CLI- and ACS-assigned values overwrite each other, whichever is assigned later.
This task is required when the ACS uses HTTPS for secure access. CWMP uses HTTP or HTTPS for data transmission. When HTTPS is used, the ACS URL begins with https://. You must specify an SSL client policy for the CPE to authenticate the ACS for HTTPS connection establishment.
Before you perform this task, first create an SSL client policy. For more information about configuring SSL client policies, see Security Configuration Guide.
2. Enter CWMP view.
cwmp
3. Specify an SSL client policy.
ssl client-policy policy-name
By default, no SSL client policy is specified.
To protect the CPE against unauthorized access, configure a CPE username and password for ACS authentication. When an ACS initiates a connection to the CPE, the ACS must provide the correct username and password.
2. Enter CWMP view.
cwmp
3. Configure the username for authentication to the CPE.
cwmp cpe username username
By default, no username has been configured for authentication to the CPE.
4. (Optional.) Configure the password for authentication to the CPE.
cwmp cpe password { cipher | simple } string
By default, no password has been configured for authentication to the CPE.
The password setting is optional. You can specify only a username for authentication.
The ACS can use the provision code to identify services assigned to each CPE. For correct configuration deployment, make sure the same provision code is configured on the CPE and the ACS. For information about the support of your ACS for provision codes, see the ACS documentation.
2. Enter CWMP view.
cwmp
3. Configure the provision code.
cwmp cpe provision-code provision-code
The default provision code is PROVISIONINGCODE.
The CWMP connection interface is the interface that the CPE uses to communicate with the ACS. To establish a CWMP connection, the CPE sends the IP address of this interface in the Inform messages, and the ACS replies to this IP address.
Typically, the CPE selects the CWMP connection interface automatically. If the CWMP connection interface is not the interface that connects the CPE to the ACS, the CPE fails to establish a CWMP connection with the ACS. In this case, you need to manually set the CWMP connection interface.
2. Enter CWMP view.
cwmp
3. Specify the interface that connects to the ACS as the CWMP connection interface.
cwmp cpe connect interface interface-type interface-number
By default, no interface is specified for CPE to connect to ACS.
You can configure the CPE to connect to the ACS periodically, or at a scheduled time for configuration or software update.
The CPE retries a connection automatically when one of the following events occurs:
· The CPE fails to connect to the ACS. The CPE considers a connection attempt as having failed when the close-wait timer expires. This timer starts when the CPE sends an Inform request. If the CPE fails to receive a response before the timer expires, the CPE resends the Inform request.
· The connection is disconnected before the session on the connection is completed.
To protect system resources, limit the number of retries that the CPE can make to connect to the ACS.
Configuring the periodic Inform feature
2. Enter CWMP view.
cwmp
3. Enable the periodic Inform feature.
cwmp cpe inform interval enable
By default, this function is disabled.
4. Set the Inform interval.
cwmp cpe inform interval interval
By default, the CPE sends an Inform message to start a session every 600 seconds.
Scheduling a connection initiation
2. Enter CWMP view.
cwmp
3. Schedule a connection initiation.
cwmp cpe inform time time
By default, no connection initiation has been scheduled.
Setting the maximum number of connection retries
2. Enter CWMP view.
cwmp
3. Set the maximum number of connection retries.
cwmp cpe connect retry retries
By default, the CPE retries a failed connection until the connection is established.
The close-wait timer specifies the following:
· The maximum amount of time the CPE waits for the response to a session request. The CPE determines that its session attempt has failed when the timer expires.
· The amount of time the connection to the ACS can be idle before it is terminated. The CPE terminates the connection to the ACS if no traffic is sent or received before the timer expires.
2. Enter CWMP view.
cwmp
3. Set the close-wait timer.
cwmp cpe wait timeout seconds
By default, the close-wait timer is 30 seconds.
For the connection request initiated from the ACS to reach the CPE, you must enable NAT traversal on the CPE when a NAT gateway resides between the CPE and the ACS.
The NAT traversal feature complies with RFC 3489 Simple Traversal of UDP Through NATs (STUN). The feature enables the CPE to discover the NAT gateway, and obtain an open NAT binding (a public IP address and port binding) through which the ACS can send unsolicited packets. The CPE sends the binding to the ACS when it initiates a connection to the ACS. For the connection requests sent by the ACS at any time to reach the CPE, the CPE maintains the open NAT binding. For more information about NAT, see NAT Configuration Guide.
2. Enter CWMP view.
cwmp
3. Enable NAT traversal.
cwmp cpe stun enable
By default, NAT traversal is disabled on the CPE.
Task |
Command |
Display CWMP configuration. |
display cwmp configuration |
Display the current status of CWMP. |
display cwmp status |
CWMP configuration examples
Example: Configuring CWMP
As shown in Figure 4, use H3C IMC BIMS as the ACS to bulk-configure the devices (CPEs), and assign ACS attributes to the CPEs from the DHCP server.
The configuration files for the CPEs in equipment rooms A and B are configure1.cfg and configure2.cfg, respectively.
Table 4 shows the ACS attributes for the CPEs to connect to the ACS.
Item |
Setting |
Preferred ACS URL |
https://10.185.10.41:9090 |
ACS username |
admin |
ACS password |
12345 |
Table 5 lists serial numbers of the CPEs.
Room |
Device |
Serial number |
A |
CPE 1 |
210231A95YH10C000045 |
CPE 2 |
210235AOLNH12000010 |
CPE 3 |
210235AOLNH12000015 |
B |
CPE 4 |
210235AOLNH12000017 |
CPE 5 |
210235AOLNH12000020 |
CPE 6 |
210235AOLNH12000022 |
Configuring the ACS
Configurations for ACS servers vary by models. For more information, see the ACS server user guide.
Configuring the DHCP server
In this example, an H3C device is operating as the DHCP server.
1. Configure an IP address pool to assign IP addresses and DNS server address to the CPEs. This example uses subnet 10.185.10.0/24 for IP address assignment.
# Enable DHCP.
<DHCP_server> system-view
[DHCP_server] dhcp enable
# Enable DHCP server on VLAN-interface 1.
[DHCP_server] interface vlan-interface 1
[DHCP_server-Vlan-interface1] dhcp select server
[DHCP_server-Vlan-interface1] quit
# Exclude the DNS server address 10.185.10.60 and the ACS IP address 10.185.10.41 from dynamic allocation.
[DHCP_server] dhcp server forbidden-ip 10.185.10.41
[DHCP_server] dhcp server forbidden-ip 10.185.10.60
# Create IP address pool 0.
[DHCP_server] ip pool 0
# Assign subnet 10.185.10.0/24 to the address pool, and specify the DNS server address 10.185.10.60 in the address pool.
[DHCP_server-ip-pool-0] network 10.185.10.0 mask 255.255.255.0
[DHCP_server-ip-pool-0] dns-list 10.185.10.60
2. Configure DHCP Option 43 to contain the ACS URL, username, and password in hexadecimal format.
[DHCP_server-ip-pool-0] option 43 hex 013B68747470733A2F2F6163732E64617461626173653A393039302F616373207669636B79203132333435
Configuring the DNS server
Map https://acs.database:9090 to https://10.185.1.41:9090 on the DNS server. For more information about DNS configuration, see DNS server documentation.
Connecting the CPEs to the network
# Connect a network cable to CPE 1 and then power on the CPE.
# Log in to CPE 1 and configure Ten-GigabitEthernet 0/0/15 to use DHCP for IP address acquisition. At startup, the CPE obtains the IP address and ACS information from the DHCP server to initiate a connection to the ACS. After the connection is established, the CPE interacts with the ACS to complete autoconfiguration.
<CPE1> system-view
[CPE1] interface ten-gigabitethernet 0/0/15
[CPE1-Ten-GigabitEthernet0/0/15] ip address dhcp-alloc
# Repeat the previous steps to connect other CPEs to the network.
# Execute the display current-configuration command on each CPE to verify that the running configurations on the CPE are the same as the configurations in the configuration file issued by the ACS.