05-Network Connectivity Command Reference
HomeSupportWirelessWX3800X Series Access ControllersReference GuidesCommand ReferencesH3C WX3800X Series Access Controllers Command References(R1411P02)-6W10005-Network Connectivity Command Reference
16-DNS commands
16-DNS commands 142.54 KB
DNS commands
display dns domain
Use display dns domain to display the domain name suffixes.
display dns domain [ dynamic ]
dynamic: Displays the domain name suffixes dynamically obtained through DHCP or other protocols. If you do not specify this keyword, the command displays the statically configured and dynamically obtained domain name suffixes.
# Display the statically configured and dynamically obtained domain name suffixes for the public network.
<Sysname> display dns domain
Type:
  D: Dynamic    S: Static
No.    Type   Domain suffix
1      S      com
2      D      net
No.
Sequence number.
Domain name suffix type:
·     S—A statically configured domain name suffix.
·     D—A domain name suffix dynamically obtained through DHCP or other protocols.
Domain suffix
Domain name suffixes.
dns domain
display dns host
Use display dns host to display information about domain name-to-IP address mappings.
display dns host [ ip | ipv6 ]
ip: Specifies type A queries. A type A query resolves a domain name to the mapped IPv4 address.
ipv6: Specifies type AAAA queries. A type AAAA query resolves a domain name to the mapped IPv6 address.
If you do not specify the ip or ipv6 keyword, this command displays domain name-to-IP address mappings of all query types.
# Display domain name-to-IP address mappings of all query types in the static domain name resolution table and dynamic domain name resolution cache for the public network.
<Sysname> display dns host
Type:
Total number: 4
No.  Host name      Type TTL       Query type IP addresses      OutInterface
1    sample.com     D    3132      A          192.168.10.1      -
                                              192.168.10.2
                                              192.168.10.3
2    sample1.com    D    2400(a)   A          100.10.23.1
3    zig.sample.com S    -         A          192.168.1.1
4    sample.net     S    -         AAAA       FE80::4904:4448
No.
Sequence number.
Host name
Domain name.
Domain name-to-IP address mapping type:
·     S—A static mapping configured by the ip host or ipv6 host command.
·     D—A mapping dynamically obtained through dynamic domain name resolution.
TTL
Time in seconds that a mapping can be stored in the cache. (a) means that the aging time is set by the dns host aging-time command. If the DNS entry is permanently valid, this field displays Infinite.
For a static mapping, this field displays a hyphen (-).
Query type
Query type: A and AAAA.
IP addresses
Replied IP address:
·     For a type A query, the replied IP address is an IPv4 address.
·     For a type AAAA query, the replied IP address is an IPv6 address.
OutInterface
Output interface specified by an application for DNS protocol packets. This field displays a hyphen (-) if the application does not specify an output interface.
ip host
ipv6 host
reset dns host
display dns server
Use display dns server to display IPv4 DNS server information.
display dns server [ dynamic ]
dynamic: Displays IPv4 DNS server information dynamically obtained through DHCP or other protocols. If you do not specify this keyword, the command displays statically configured and dynamically obtained IPv4 DNS server information.
# Display IPv4 DNS server information for the public network.
<Sysname> display dns server
Type:
No. Type  IP address
1   S     202.114.0.124
2   S     169.254.65.125
No.
Sequence number.
DNS server type:
·     S—A manually configured DNS server.
·     D—DNS server information dynamically obtained through DHCP or other protocols.
IP address
IPv4 address of the DNS server.
dns server
display ipv6 dns server
Use display ipv6 dns server to display IPv6 DNS server information.
display ipv6 dns server [ dynamic ]
dynamic: Displays IPv6 DNS server information dynamically obtained through DHCP or other protocols. If you do not specify this keyword, the command displays the statically configured and dynamically obtained IPv6 DNS server information.
# Display IPv6 DNS server information for the public network.
<Sysname> display ipv6 dns server
Type:
No. Type  IPv6 address                             Outgoing Interface
1   S     2::2
No.
Sequence number.
DNS server type:
IPv6 address
IPv6 address of the DNS server.
Outgoing Interface
Output interface.
ipv6 dns server
dns domain
Use dns domain to configure a domain name suffix.
Use undo dns domain to delete the specified domain name suffix.
dns domain domain-name
undo dns domain domain-name
No domain name suffix is configured. Only the provided domain name is resolved.
domain-name: Specifies a domain name suffix. It is a dot-separated, case-insensitive string that can include letters, digits, hyphens (-), underscores (_), and dots (.), for example, example.com. The domain name suffix can include a maximum of 253 characters, and each separated string includes no more than 63 characters.
For domain name resolution, the resolver automatically uses the suffix list to supply the missing part of an incomplete name entered by a user.
A domain name suffix applies to both IPv4 DNS and IPv6 DNS.
The system allows a maximum of 16 domain name suffixes for the public network.
# Configure domain name suffix com for the public network.
[Sysname] dns domain com
display dns domain
dns dscp
Use dns dscp to set the DSCP value for DNS packets sent by a DNS client or DNS proxy.
Use undo dns dscp to restore the default.
dns dscp dscp-value
undo dns dscp
The DSCP value is 0 in DNS packets sent by a DNS client or DNS proxy.
dscp-value: Specifies the DSCP value in the range of 0 to 63.
The DSCP value of a packet specifies the priority level of the packet and affects the transmission priority of the packet. A bigger DSCP value represents a higher priority.
# Set the DSCP value to 30 for outgoing DNS packets.
[Sysname] dns dscp 30
dns fast-reply enable
Use dns fast-reply enable to enable DNS fast-reply.
Use undo dns fast-reply enable to disable DNS fast-reply.
DNS fast-reply is disabled.
As DNS fast-reply can process a large number of DNS requests per second, use this feature in scenarios that require high DNS packet processing performance.
With this feature enabled, the device monitors the received DNS requests (only UDP packets are supported in the current software version). Then, it resolves the domain names in the requests, and searches for a match in the local static domain name resolution table, DNS cache, and dynamic domain name resolution cache.
·     If a match is found, the device sends a DNS reply to the DNS client.
·     If no match is found, the device forwards the query to the DNS server.
This command enables both IPv4 DNS fast-reply and IPv6 DNS fast-reply.
This command does not take effect on labeled DNS packets.
# Enable DNS fast-reply.
[Sysname] dns fast-reply enable
dns host aging-time
Use dns host aging-time to set the aging time for a specified domain name.
Use undo dns host aging-time to restore the default.
dns host host-name aging-time { time-value | infinite }
undo dns host host-name aging-time
The aging time for a domain name is the TTL in the DNS reply.
host host-name: Specifies a domain name. It is a dot-separated, case-insensitive string that can include letters, digits, hyphens (-), underscores (_), and dots (.), for example, www.example.com. The domain name can include a maximum of 253 characters, and each separated string includes no more than 63 characters.
aging-time time-value: Specifies the aging time in seconds. The value range for this argument is 1 to 604800.
aging-time infinite: Specifies a permanently valid domain name.
The DNS server determines how long a DNS entry is valid, and the DNS client obtains the aging information from DNS responses. To set the aging time, execute the dns host aging-time command.
With this command configured, the device searches the DNS cache and dynamic domain name resolution cache, and changes the TTL in all entries into the specified aging time.
To restore the default, execute the undo dns host aging-time command. The restored aging time is the original TTL in the DNS reply. The corresponding DNS entry is removed if the original TTL expires after executing the command.
You can set a maximum of 256 times of aging time for domain names.
# Set the aging time for domain name www.example.com on the public network to 3600 seconds.
[Sysname] dns host www.example.com aging-time 3600
display arp timer aging
dns proxy enable
Use dns proxy enable to enable DNS proxy.
Use undo dns proxy enable to disable DNS proxy.
dns proxy enable
DNS proxy is disabled.
This configuration applies to both IPv4 DNS and IPv6 DNS.
# Enable DNS proxy.
[Sysname] dns proxy enable
dns server
Use dns server to specify the IPv4 address of a DNS server.
Use undo dns server to remove the IPv4 address of a DNS server.
dns server ip-address
undo dns server [ ip-address ]
No DNS server IPv4 address is specified.
Interface view
ip-address: Specifies the IPv4 address of a DNS server. When you execute the undo form of the command in interface view, you must specify this argument.
The device sends a DNS query request to the DNS servers in the order their IPv4 addresses are specified.
The system allows a maximum of six DNS server IPv4 addresses for the public network.
If you do not specify an IPv4 address, the undo dns server command removes all DNS server IPv4 addresses for the public network.
# Specify DNS server IPv4 address 172.16.1.1.
[Sysname] dns server 172.16.1.1
# Specify DNS server IPv4 address 172.16.1.1 on VLAN-interface 2.
[Sysname-Vlan-interface2] dns server 172.16.1.1
display dns server
dns snooping enable
Use dns snooping enable to enable DNS snooping.
Use undo dns snooping enable to disable DNS snooping.
dns snooping enable [ authorizing ]
DNS snooping is disabled.
authorizing: Provides the DNS snooping service for DNS requests from users in authorizing state.
Application scenarios
DNS snooping is applicable to the scenario where traffic filtering is based on domain names.
Operating mechanism
Other modules (for example, the address object group module) can obtain the IP addresses corresponding to domain names through DNS snooping only after they send domain name subscription requests to the DNS module.
Enabled with DNS snooping, the device monitors received DNS requests and replies, and works as follows:
·     If the domain name in a DNS request matches a subscribed domain name, the device records the DNS mapping after receiving the DNS reply, and reports the mapping to the corresponding module for traffic filtering.
·     If the domain name does not match a subscribed domain name, the device does not record the DNS mapping.
When the domain names subscribed to by other modules age out, the DNS module notifies the modules of deleting the corresponding mappings to ensure mapping accuracy.
Recommended configuration
In the scenario where traffic filtering is based on domain names, the device resolves all DNS packets and the object group determines whether to permit packets after resolution. This causes low packet processing efficiency and consumes a lot of CPU resources.
To resolve such an issue, specify the authorizing keyword when you execute this command. The device then applies DNS snooping only to DNS requests from authenticated users (access users that have the ACL and redirect URL authorization attributes) and permits other DNS requests to alleviate pressure and reduce CPU usage.
DNS snooping only works between the DNS client and DNS server, or the DNS client and DNS proxy.
The DNS snooping and DNS transparent proxy features cannot be both configured.
The dns snooping enable and dns snooping enable authorizing commands are mutually exclusive.
The dns snooping enable authorizing command takes effect only when the DNS client and DNS snooping reside in the same LAN.
# Enable DNS snooping.
[Sysname] dns snooping enable
dns transparent-proxy enable
dns source-interface
Use dns source-interface to specify the source interface for DNS packets.
Use undo dns source-interface to restore the default.
dns source-interface interface-type interface-number
undo dns source-interface interface-type interface-number
No source interface is specified for DNS packets. The device uses the primary IP address of the output interface of the matching route as the source IP address for a DNS request.
This configuration applies to both IPv4 and IPv6.
In IPv4 DNS, the device uses the primary IPv4 address of the specified source interface as the source IP address of a DNS query. In IPv6 DNS, the device selects an IPv6 address of the specified source interface as the source IP address of a DNS query. The method of selecting the IPv6 address is defined in RFC 3484.
The system allows only one source interface for the public network. If you execute this command multiple times, the most recent configuration takes effect.
As a best practice, do not specify an automatically generated interface (for example, an automatic tunnel interface) as the source interface for DNS packets. Otherwise, configuration might fail or might be lost.
# Specify VLAN-interface 2 as the source interface for DNS packets on the public network.
[Sysname] dns source-interface vlan-interface 2
dns spoofing
Use dns spoofing to enable DNS spoofing and specify the IPv4 address for spoofing DNS requests.
Use undo dns spoofing to disable DNS spoofing.
dns spoofing ip-address
undo dns spoofing ip-address
DNS spoofing is disabled.
ip-address: Specifies the IPv4 address used to spoof DNS requests.
Use the dns spoofing command together with the dns proxy enable command.
DNS spoofing functions when the DNS proxy does not know the DNS server address or cannot reach the DNS server. It enables the DNS proxy to spoof DNS queries of type A by responding with the specified IPv4 address.
The system allows only one replied IPv4 address for the public network. If you execute this command multiple times, the most recent configuration takes effect.
# Enable DNS spoofing for the public network and specify IPv4 address 1.1.1.1 for spoofing DNS requests.
[Sysname] dns spoofing 1.1.1.1
dns proxy enable
dns trust-interface
Use dns trust-interface to specify a DNS trusted interface.
Use undo dns trust-interface to remove a DNS trusted interface.
dns trust-interface interface-type interface-number
undo dns trust-interface [ interface-type interface-number ]
No DNS trusted interface is specified.
By default, an interface obtains DNS suffix and DNS server information from DHCP. A network attacker might act as the DHCP server to assign a wrong DNS suffix and DNS server address to the device. As a result, the device fails to obtain the resolved IP address or might get the wrong IP address. With the DNS trusted interface specified, the device only uses the DNS suffix and DNS server information obtained through the trusted interface to avoid attacks.
You can configure a maximum of 128 DNS trusted interfaces on the device.
If you do not specify an interface, the undo dns trust-interface command removes all DNS trusted interfaces and restores the default.
# Specify VLAN-interface 2 as a DNS trusted interface.
[Sysname] dns trust-interface vlan-interface 2
ip host
Use ip host to create a host name-to-IPv4 address mapping.
Use undo ip host to remove a host name-to-IPv4 address mapping.
ip host host-name ip-address
undo ip host host-name ip-address
No host name-to-IPv4 address mappings exist.
host-name: Specifies a host name, a case-insensitive string of 1 to 253 characters. Valid characters are letters, digits, hyphens (-), underscores (_), and dots (.).
ip-address: Specifies the IPv4 address of the host.
The system allows a maximum of 1024 host name-to-IPv4 address mappings for the public network.
For the public network, each host name maps to only one IPv4 address. If you execute this command multiple times, the most recent configuration takes effect.
Do not use the ping command parameter ip, -a, -c, -f, -h, -i, -m, -n, -p, -q, -r, -s, -t, -tos, or -v as the host name. For more information about the ping command parameters, see Network Management and Monitoring Command Reference.
# Map IPv4 address 10.110.0.1 to host name aaa for the public network.
[Sysname] ip host aaa 10.110.0.1
display dns host
ipv6 dns dscp
Use ipv6 dns dscp to set the DSCP value for IPv6 DNS packets sent by an IPv6 DNS client or IPv6 DNS proxy.
Use undo ipv6 dns dscp to restore the default.
ipv6 dns dscp dscp-value
undo ipv6 dns dscp
The DSCP value is 0 in IPv6 DNS packets sent by an IPv6 DNS client or IPv6 DNS proxy.
# Set the DSCP value to 30 for outgoing IPv6 DNS packets.
[Sysname] ipv6 dns dscp 30
ipv6 dns server
Use ipv6 dns server to specify the IPv6 address of a DNS server.
Use undo ipv6 dns server to remove the IPv6 address of a DNS server.
ipv6 dns server ipv6-address [ interface-type interface-number ]
undo ipv6 dns server [ ipv6-address [ interface-type interface-number ] ]
No DNS server IPv6 address is specified.
ipv6-address: Specifies the IPv6 address of a DNS server.
interface-type interface-number: Specifies the output interface by its type and number. If you do not specify an interface, the device forwards DNS packets out of the output interface of the matching route. Specify this argument if the IPv6 address of the DNS server is a link-local address. Do not specify this argument if the IPv6 address of the DNS server is a global unicast address.
For dynamic DNS, the device sends a DNS query request to the DNS servers in the order their IPv6 addresses are specified.
The system allows a maximum of six DNS server IPv6 addresses for the public network.
If you do not specify an IPv6 address, the undo ipv6 dns server command removes all DNS server IPv6 addresses for the public network.
# Specify DNS server IPv6 address 2002::1 for the public network.
[Sysname] ipv6 dns server 2002::1
ipv6 dns spoofing
Use ipv6 dns spoofing to enable DNS spoofing and specify the IPv6 address to spoof DNS requests.
Use undo ipv6 dns spoofing to disable DNS spoofing.
ipv6 dns spoofing ipv6-address
undo ipv6 dns spoofing ipv6-address
ipv6-address: Specifies the IPv6 address used to spoof DNS requests.
Use the ipv6 dns spoofing command together with the dns proxy enable command.
DNS spoofing functions when the DNS proxy does not know the DNS server address or cannot reach the DNS server. It enables the DNS proxy to spoof DNS queries of type AAAA by responding with the specified IPv6 address.
The system allows only one replied IPv6 address for the public network. If you execute this command multiple times, the most recent configuration takes effect.
# Enable DNS spoofing for the public network and specify IPv6 address 2001::1 for spoofing DNS requests.
[Sysname] ipv6 dns spoofing 2001::1
dns proxy enable
ipv6 host
Use ipv6 host to create a host name-to-IPv6 address mapping.
Use undo ipv6 host to remove a host name-to-IPv6 address mapping.
ipv6 host host-name ipv6-address
undo ipv6 host host-name ipv6-address
No host name-to-IPv6 address mappings exist.
host-name: Specifies a host name, a case-insensitive string of 1 to 253 characters. It can include letters, digits, hyphens (-), underscores (_), and dots (.).
ipv6-address: Specifies the IPv6 address of the host.
The system allows a maximum of 1024 host name-to-IPv6 address mappings for the public network.
For the public network, each host name maps to only one IPv6 address. If you execute this command multiple times, the most recent configuration takes effect.
Do not use the ping ipv6 command parameter -a, -c, -i, -m, -q, -s, -t, -tc, or -v as the host name. For more information about the ping ipv6 command parameters, see Network Management and Monitoring Command Reference.
# Map IPv6 address 2001::1 to host name aaa for the public network.
[Sysname] ipv6 host aaa 2001::1
ip host
reset dns host
Use reset dns host to clear dynamic DNS entries.
reset dns host [ ip | ipv6 ]
If you do not specify the ip or ipv6 keyword, the reset dns host command clears dynamic DNS entries of all query types.
# Clear dynamic DNS entries of all query types for the public network.
<Sysname> reset dns host
display dns host