Configuring CWMP

About CWMP

CPE WAN Management Protocol (CWMP), also called "TR-069," is a DSL Forum technical specification for remote management of network devices.

The protocol was initially designed to provide remote autoconfiguration through a server for large numbers of dispersed end-user devices in a network. CWMP can be used on different types of networks, including Ethernet.

CWMP network framework

Figure 1 shows a basic CWMP network framework.

Figure 1 CWMP network framework

A basic CWMP network includes the following network elements:

·     ACS—Autoconfiguration server, the management device in the network.

·     CPE—Customer premises equipment, the managed device in the network.

·     DNS server—Domain name system server. CWMP defines that the ACS and the CPE use URLs to identify and access each other. DNS is used to resolve the URLs.

·     DHCP server—Assigns ACS attributes along with IP addresses to CPEs when the CPEs are powered on. DHCP server is optional in CWMP. With a DHCP server, you do not need to configure ACS attributes manually on each CPE. The CPEs can contact the ACS automatically when they are powered on for the first time.

The device is operating as a CPE in the CWMP framework.

Basic CWMP functions

You can autoconfigure and upgrade CPEs in bulk from the ACS.

Autoconfiguration

You can create configuration files for different categories of CPEs on the ACS. Based on the device models and serial numbers of the CPEs, the ACS verifies the categories of the CPEs and issues the associated configuration to them.

The following are methods available for the ACS to issue configuration to the CPE:

·     Transfers the configuration file to the CPE, and specifies the file as the next-startup configuration file. At a reboot, the CPE starts up with the ACS-specified configuration file.

·     Runs the configuration in the CPE's RAM. The configuration takes effect immediately on the CPE. For the running configuration to survive a reboot, you must save the configuration on the CPE.

CPE software management

The ACS can manage CPE software upgrade.

When the ACS finds a software version update, the ACS notifies the CPE to download the software image file from a specific location. The location can be the URL of the ACS or an independent file server.

If the CPE successfully downloads the software image file and the file is validated, the CPE notifies the ACS of a successful download. If the CPE fails to download the software image file or the file is invalidated, the CPE notifies the ACS of an unsuccessful download.

Data backup

The ACS can require the CPE to upload a configuration file or log file to a specific location. The destination location can be the ACS or a file server.

CPE status and performance monitoring

The ACS can monitor the status and performance of CPEs. Table 1 shows the available CPE status and performance objects for the ACS to monitor.

Table 1 CPE status and performance objects available for the ACS to monitor

Category

Objects

Remarks

Device information

Manufacturer

ManufacturerOUI

SerialNumber

HardwareVersion

SoftwareVersion

N/A

Operating status and information

DeviceStatus

UpTime

N/A

Configuration file

ConfigFile

Local configuration file stored on CPE for upgrade. The ACS can issue configuration to the CPE by transferring a configuration file to the CPE or running the configuration in CPE's RAM.

CWMP settings

ACS URL

URL address of the ACS to which the CPE initiates a CWMP connection. This object is also used for main/backup ACS switchover.

ACS username

ACS password

When the username and password of the ACS are changed, the ACS changes the ACS username and password on the CPE to the new username and password.

When a main/backup ACS switchover occurs, the main ACS also changes the ACS username and password to the backup ACS username and password.

PeriodicInformEnable

Whether to enable or disable the periodic Inform feature.

PeriodicInformInterval

Interval for periodic connection from the CPE to the ACS for configuration and software update.

PeriodicInformTime

Scheduled time for connection from the CPE to the ACS for configuration and software update.

ConnectionRequestURL (CPE URL)

N/A

ConnectionRequestUsername (CPE username)

ConnectionRequestPassword (CPE password)

CPE username and password for authentication from the ACS to the CPE.

How CWMP works

RPC methods

CWMP uses remote procedure call (RPC) methods for bidirectional communication between CPE and ACS. The RPC methods are encapsulated in HTTP or HTTPS.

Table 2 shows the primary RPC methods used in CWMP.

Table 2 RPC methods

RPC method

Description

Get

The ACS obtains the values of parameters on the CPE.

Set

The ACS modifies the values of parameters on the CPE.

Inform

The CPE sends an Inform message to the ACS for the following purposes:

·     Initiates a connection to the ACS.

·     Reports configuration changes to the ACS.

·     Periodically updates CPE settings to the ACS.

Download

The ACS requires the CPE to download a configuration or software image file from a specific URL for software or configuration update.

Upload

The ACS requires the CPE to upload a file to a specific URL.

Reboot

The ACS reboots the CPE remotely for the CPE to complete an upgrade or recover from an error condition.

Autoconnect between ACS and CPE

The CPE automatically initiates a connection to the ACS when one of the following events occurs:

·     ACS URL change. The CPE initiates a connection request to the new ACS URL.

·     CPE startup. The CPE initiates a connection to the ACS after the startup.

·     Timeout of the periodic Inform interval. The CPE re-initiates a connection to the ACS at the Inform interval.

·     Expiration of the scheduled connection initiation time. The CPE initiates a connection to the ACS at the scheduled time.

CWMP connection establishment

Step 1 through step 5 in Figure 2 show the procedure of establishing a connection between the CPE and the ACS.

1.     After obtaining the basic ACS parameters, the CPE initiates a TCP connection to the ACS.

2.     If HTTPS is used, the CPE and the ACS initialize SSL for a secure HTTP connection.

3.     The CPE sends an Inform message in HTTPS to initiate a CWMP session.

4.     After the CPE passes authentication, the ACS returns an Inform response to establish the session.

5.     After sending all requests, the CPE sends an empty HTTP post message.

Figure 2 CWMP connection establishment

Main/backup ACS switchover

Typically, two ACSs are used in a CWMP network for consecutive monitoring on CPEs. When the main ACS needs to reboot, it points the CPE to the backup ACS. Step 6 through step 11 in Figure 3 show the procedure of a main/backup ACS switchover.

1.     Before the main ACS reboots, it queries the ACS URL set on the CPE.

2.     The CPE replies with its ACS URL setting.

3.     The main ACS sends a Set request to change the ACS URL on the CPE to the backup ACS URL.

4.     After the ACS URL is modified, the CPE sends a response.

5.     The main ACS sends an empty HTTP message to notify the CPE that it has no other requests.

6.     The CPE closes the connection, and then initiates a new connection to the backup ACS URL.

Figure 3 Main and backup ACS switchover

Restrictions and guidelines: CWMP configuration

CWMP is available only in IPv4 networks. If you configure CWMP in an IPv6 network, the feature does not take effect.

You can configure ACS and CPE attributes from the CPE's CLI, the DHCP server, or the ACS. For an attribute, the CLI- and ACS-assigned values have higher priority than the DHCP-assigned value. The CLI- and ACS-assigned values overwrite each other, whichever is assigned later.

This document only describes configuring ACS and CPE attributes from the CLI and DHCP server. For more information about configuring and using the ACS, see ACS documentation.

CWMP tasks at a glance

To configure CWMP, perform the following tasks:

1.     Enabling CWMP from the CLI

You can also enable CWMP from a DHCP server.

2.     Configuring ACS attributes

a.     Configuring the preferred ACS attributes

b.     (Optional.) Configuring the default ACS attributes from the CLI

3.     Configuring CPE attributes

a.     Specifying an SSL client policy for HTTPS connection to ACS

This task is required when the ACS uses HTTPS for secure access.

b.     (Optional.) Configuring ACS authentication parameters

c.     (Optional.) Configuring the provision code

d.     (Optional.) Configuring the CWMP connection interface

e.     (Optional.) Configuring autoconnect parameters

f.     (Optional.) Setting the close-wait timer

g.     (Optional.) Enabling NAT traversal for the CPE

Enabling CWMP from the CLI

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Enable CWMP.

cwmp enable

By default, CWMP is disabled.

Configuring ACS attributes

About ACS attributes

You can configure two sets of ACS attributes for the CPE: preferred and default.

·     The preferred ACS attributes are configurable from the CPE's CLI, the DHCP server, and ACS.

·     The default ACS attributes are configurable only from the CLI.

If the preferred ACS attributes are not configured, the CPE uses the default ACS attributes for connection establishment.

Configuring the preferred ACS attributes

Assigning ACS attributes from the DHCP server

The DHCP server in a CWMP network assigns the following information to CPEs:

·     IP addresses for the CPEs.

·     DNS server address.

·     ACS URL and ACS login authentication information.

This section introduces how to use DHCP option 43 to assign the ACS URL and ACS login authentication username and password. For more information about DHCP and DNS, see Layer 3—IP Services Configuration Guide.

If the DHCP server is an H3C device, you can configure DHCP option 43 by using the option 43 hex 01length URL username password command.

·     length—A hexadecimal number that indicates the total length of the length, URL, username, and password arguments, including the spaces between these arguments. No space is allowed between the 01 keyword and the length value.

·     URL—ACS URL.

·     username—Username for the CPE to authenticate to the ACS.

·     password—Password for the CPE to authenticate to the ACS.

 

 

NOTE:

The ACS URL, username and password must use the hexadecimal format and be space separated.

The following example configures the ACS address as https://169.254.76.31:7547/acs, username as 1234, and password as 5678:

<Sysname> system-view

[Sysname] dhcp server ip-pool 0

[Sysname-dhcp-pool-0] option 43 hex 012368747470733A2F2F3136392E3235342E37362E33313A3735343720313233342035363738

Table 3 Hexadecimal forms of the ACS attributes

Attribute

Attribute value

Hexadecimal form

Length

39 characters

27

ACS URL

https://169.254.76.31:7547/acs

68747470733A2F2F3136392E3235342E37362E33313A3735343720

NOTE:

The two ending digits (20) represent the space.

ACS connect username

1234

3132333420

NOTE:

The two ending digits (20) represent the space.

ACS connect password

5678

35363738

Configuring the preferred ACS attributes from the CLI

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Configure the preferred ACS URL.

cwmp acs url url

By default, no preferred ACS URL has been configured.

4.     Configure the username for authentication to the preferred ACS URL.

cwmp acs username username

By default, no username has been configured for authentication to the preferred ACS URL.

5.     (Optional.) Configure the password for authentication to the preferred ACS URL.

cwmp acs password { cipher | simple } string

By default, no password has been configured for authentication to the preferred ACS URL.

Configuring the default ACS attributes from the CLI

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Configure the default ACS URL.

cwmp acs default url url

By default, no default ACS URL has been configured.

4.     Configure the username for authentication to the default ACS URL.

cwmp acs default username username

By default, no username has been configured for authentication to the default ACS URL.

5.     (Optional.) Configure the password for authentication to the default ACS URL.

cwmp acs default password { cipher | simple } string

By default, no password has been configured for authentication to the default ACS URL.

Configuring CPE attributes

About CPE attributes

You can configure the following CPE attributes only from the CPE's CLI.

·     CWMP connection interface.

·     NAT traversal.

·     Maximum number of connection retries.

·     SSL client policy for HTTPS connection to ACS.

For other CPE attribute values, you can assign them to the CPE from the CPE's CLI or the ACS. The CLI- and ACS-assigned values overwrite each other, whichever is assigned later.

Specifying an SSL client policy for HTTPS connection to ACS

About this task

This task is required when the ACS uses HTTPS for secure access. CWMP uses HTTP or HTTPS for data transmission. When HTTPS is used, the ACS URL begins with https://. You must specify an SSL client policy for the CPE to authenticate the ACS for HTTPS connection establishment.

Prerequisites

Before you perform this task, first create an SSL client policy. For more information about configuring SSL client policies, see Security Configuration Guide.

Procedure

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Specify an SSL client policy.

ssl client-policy policy-name

By default, no SSL client policy is specified.

Configuring ACS authentication parameters

About this task

To protect the CPE against unauthorized access, configure a CPE username and password for ACS authentication. When an ACS initiates a connection to the CPE, the ACS must provide the correct username and password.

Procedure

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Configure the username for authentication to the CPE.

cwmp cpe username username

By default, no username has been configured for authentication to the CPE.

4.     (Optional.) Configure the password for authentication to the CPE.

cwmp cpe password { cipher | simple } string

By default, no password has been configured for authentication to the CPE.

The password setting is optional. You can specify only a username for authentication.

Configuring the provision code

About this task

The ACS can use the provision code to identify services assigned to each CPE. For correct configuration deployment, make sure the same provision code is configured on the CPE and the ACS. For information about the support of your ACS for provision codes, see the ACS documentation.

Procedure

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Configure the provision code.

cwmp cpe provision-code provision-code

The default provision code is PROVISIONINGCODE.

Configuring the CWMP connection interface

About this task

The CWMP connection interface is the interface that the CPE uses to communicate with the ACS. To establish a CWMP connection, the CPE sends the IP address of this interface in the Inform messages, and the ACS replies to this IP address.

Typically, the CPE selects the CWMP connection interface automatically. If the CWMP connection interface is not the interface that connects the CPE to the ACS, the CPE fails to establish a CWMP connection with the ACS. In this case, you need to manually set the CWMP connection interface.

Procedure

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Specify the interface that connects to the ACS as the CWMP connection interface.

cwmp cpe connect interface interface-type interface-number

By default, no CWMP connection interface is specified.

Configuring autoconnect parameters

About this task

You can configure the CPE to connect to the ACS periodically, or at a scheduled time for configuration or software update.

The CPE retries a connection automatically when one of the following events occurs:

·     The CPE fails to connect to the ACS. The CPE considers a connection attempt as having failed when the close-wait timer expires. This timer starts when the CPE sends an Inform request. If the CPE fails to receive a response before the timer expires, the CPE resends the Inform request.

·     The connection is disconnected before the session on the connection is completed.

To protect system resources, limit the number of retries that the CPE can make to connect to the ACS.

Configuring the periodic Inform feature

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Enable the periodic Inform feature.

cwmp cpe inform interval enable

By default, this function is disabled.

4.     Set the Inform interval.

cwmp cpe inform interval interval

By default, the CPE sends an Inform message to start a session every 600 seconds.

Scheduling a connection initiation

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Schedule a connection initiation.

cwmp cpe inform time time

By default, no connection initiation has been scheduled.

Setting the maximum number of connection retries

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Set the maximum number of connection retries.

cwmp cpe connect retry retries

By default, the CPE retries a failed connection until the connection is established.

Setting the close-wait timer

About this task

The close-wait timer specifies the following:

·     The maximum amount of time the CPE waits for the response to a session request. The CPE determines that its session attempt has failed when the timer expires.

·     The amount of time the connection to the ACS can be idle before it is terminated. The CPE terminates the connection to the ACS if no traffic is sent or received before the timer expires.

Procedure

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Set the close-wait timer.

cwmp cpe wait timeout seconds

By default, the close-wait timer is 30 seconds.

Enabling NAT traversal for the CPE

About this task

For the connection request initiated from the ACS to reach the CPE, you must enable NAT traversal on the CPE when a NAT gateway resides between the CPE and the ACS.

The NAT traversal feature complies with RFC 3489 Simple Traversal of UDP Through NATs (STUN). The feature enables the CPE to discover the NAT gateway, and obtain an open NAT binding (a public IP address and port binding) through which the ACS can send unsolicited packets. The CPE sends the binding to the ACS when it initiates a connection to the ACS. For the connection requests sent by the ACS at any time to reach the CPE, the CPE maintains the open NAT binding.

Procedure

1.     Enter system view.

system-view

2.     Enter CWMP view.

cwmp

3.     Enable NAT traversal.

cwmp cpe stun enable

By default, NAT traversal is disabled on the CPE.

Display and maintenance commands for CWMP

Execute display commands in any view.

 

Task

Command

Display CWMP configuration.

display cwmp configuration

Display the current status of CWMP.

display cwmp status

CWMP configuration examples

Example: Configuring CWMP

Network configuration

As shown in Figure 4, use H3C IMC BIMS as the ACS to bulk-configure the devices (CPEs), and assign ACS attributes to the CPEs from the DHCP server.

The configuration files for the CPEs in equipment rooms A and B are configure1.cfg and configure2.cfg, respectively.

Figure 4 Network diagram

Table 4 shows the ACS attributes for the CPEs to connect to the ACS.

Table 4 ACS attributes

Item

Setting

Preferred ACS URL

https://10.185.10.41:9090

ACS username

admin

ACS password

12345

Table 5 lists serial numbers of the CPEs.

Table 5 CPE list

Room

Device

Serial number

A

CPE 1

210231A95YH10C000045

CPE 2

210235AOLNH12000010

CPE 3

210235AOLNH12000015

B

CPE 4

210235AOLNH12000017

CPE 5

210235AOLNH12000020

CPE 6

210235AOLNH12000022

Configuring the ACS

Figures in this section are for illustration only.

To configure the ACS:

1.     Log in to the ACS:

a.     Launch a Web browser on the ACS configuration terminal.

b.     In the address bar of the Web browser, enter the ACS URL and port number. This example uses https://10.185.10.41:8080/imc.

c.     On the login page, enter the ACS login username and password, and then click Login.

2.     Create a CPE group for each equipment room:

a.     Select Service > BIMS > CPE Group from the top navigation bar.

The CPE Group page appears.

Figure 5 CPE Group page

a.     Click Add.

b.     Enter a username, and then click OK.

Figure 6 Adding a CPE group

a.     Repeat the previous two steps to create a CPE group for CPEs in Room B.

3.     Add CPEs to the CPE group for each equipment room:

a.     Select Service > BIMS > Resource Management > Add CPE from the top navigation bar.

b.     On the Add CPE page, configure the following parameters:

-     Authentication Type—Select ACS UserName.

-     CPE Name—Enter a CPE name.

-     ACS Username—Enter admin.

-     ACS Password Generated—Select Manual Input.

-     ACS Password—Enter a password for ACS authentication.

-     ACS Confirm Password—Re-enter the password.

-     CPE Model—Select the CPE model.

-     CPE Group—Select the CPE group.

Figure 7 Adding a CPE

 

a.     Click OK.

b.     Verify that the CPE has been added successfully from the All CPEs page.

Figure 8 Viewing CPEs

a.     Repeat the previous steps to add CPE 2 and CPE 3 to the CPE group for Room A, and add CPEs in Room B to the CPE group for Room B.

4.     Configure a configuration template for each equipment room:

a.     Select Service > BIMS > Configuration Management > Configuration Templates from the top navigation bar.

Figure 9 Configuration Templates page

a.     Click Import.

b.     Select a source configuration file, select Configuration Segment as the template type, and then click OK.

The created configuration template will be displayed in the Configuration Template list after a successful file import.

 

IMPORTANT

IMPORTANT:

If the first command in the configuration template file is system-view, make sure no characters exist in front of the command.

Figure 10 Importing a configuration template

Figure 11 Configuration Template list

a.     Repeat the previous steps to configure a configuration template for Room B.

5.     Add software library entries:

a.     Select Service > BIMS > Configuration Management > Software Library from the top navigation bar.

Figure 12 Software Library page

a.     Click Import.

b.     Select a source file, and then click OK.

Figure 13 Importing CPE software

a.     Repeat the previous steps to add software library entries for CPEs of different models.

6.     Create an auto-deployment task for each equipment room:

a.     Select Service > BIMS > Configuration Management > Deployment Guide from the top navigation bar.

Figure 14 Deployment Guide

a.     Click By CPE Model from the Auto Deployment Configuration field.

b.     Select a configuration template, select Startup Configuration from the File Type to be Deployed list, and click Select Model to select CPEs in Room A. Then, click OK.

You can search for CPEs by CPE group.

Figure 15 Auto deployment configuration

a.     Click OK on the Auto Deploy Configuration page.

Figure 16 Operation result

a.     Repeat the previous steps to add a deployment task for CPEs in Room B.

Configuring the DHCP server

In this example, an H3C device is operating as the DHCP server.

1.     Configure an IP address pool to assign IP addresses and DNS server address to the CPEs. This example uses subnet 10.185.10.0/24 for IP address assignment.

# Enable DHCP.

<DHCP_server> system-view

[DHCP_server] dhcp enable

# Enable DHCP server on VLAN-interface 1.

[DHCP_server] interface vlan-interface 1

[DHCP_server-Vlan-interface1] dhcp select server

[DHCP_server-Vlan-interface1] quit

# Exclude the DNS server address 10.185.10.60 and the ACS IP address 10.185.10.41 from dynamic allocation.

[DHCP_server] dhcp server forbidden-ip 10.185.10.41

[DHCP_server] dhcp server forbidden-ip 10.185.10.60

# Create DHCP address pool 0.

[DHCP_server] dhcp server ip-pool 0

# Assign subnet 10.185.10.0/24 to the address pool, and specify the DNS server address 10.185.10.60 in the address pool.

[DHCP_server-dhcp-pool-0] network 10.185.10.0 mask 255.255.255.0

[DHCP_server-dhcp-pool-0] dns-list 10.185.10.60

2.     Configure DHCP Option 43 to contain the ACS URL, username, and password in hexadecimal format.

[DHCP_server-dhcp-pool-0] option 43 hex 013B68747470733A2F2F6163732E64617461626173653A393039302F616373207669636B79203132333435

Configuring the DNS server

Map https://acs.database:9090 to https://10.185.1.41:9090 on the DNS server. For more information about DNS configuration, see DNS server documentation.

Connecting the CPEs to the network

# Connect CPE 1 to the network, and then power on the CPE. (Details not shown.)

# Log in to CPE 1 and configure its VLAN-interface 2 to use DHCP for IP address acquisition and assign interface GigabitEthernet 1/0/1 to VLAN 2.

<CPE1> system-view

[CPE1] vlan 2

[CPE1-vlan2] quit

[CPE1] interface gigabitethernet 1/0/1

[CPE1-GigabitEthernet1/0/1] port access vlan 2

[CPE1-GigabitEthernet1/0/1] quit

[CPE1] interface vlan-interface 2

[CPE1-Vlan-interface2] ip address dhcp-alloc

# Repeat the previous steps to configure the other CPEs.

Verifying the configuration

# Execute the display current-configuration command to verify that the running configurations on CPEs are the same as the configurations issued by the ACS.

 

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
All Support
  • Become A Partner
  • Partner Policy & Program
  • Global Learning
  • Partner Sales Resources
  • Partner Business Management
  • Service Business
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us
新华三官网