22-EVPN Configuration Guide
HomeSupportConfigure & DeployConfiguration GuidesH3C MSR610[810][830][1000S][2600][3600] Routers @CG@(V7)-R6749-6W10022-EVPN Configuration Guide
02-EVPN-DCI configuration
02-EVPN-DCI configuration 525.80 KB
Configuring EVPN-DCI
About EVPN-DCI
EVPN data center interconnect (EVPN-DCI) uses VXLAN-DCI tunnels to provide connectivity for data centers over an IP transport network.
EVPN-DCI network model
As shown in Figure 1, the EVPN-DCI network contains VTEPs and edge devices (EDs) located at the edge of the transport network. A VXLAN tunnel is established between a VTEP and an ED, and a VXLAN-DCI tunnel is established between two EDs. VXLAN-DCI tunnels use VXLAN encapsulation. Each ED de-encapsulates incoming VXLAN packets and re-encapsulates them based on the destination before forwarding the packets through a VXLAN or VXLAN-DCI tunnel.
Figure 1 EVPN-DCI network model
Working mechanisms
In an EVPN-DCI network, BGP EVPN peer relationships are established between EDs and between EDs and VTEPs. When advertising routes to a VTEP or another ED, an ED replaces the routes' nexthop IP address and router MAC address with its IP address and router MAC address.
In an EVPN-DCI network, a VTEP and an ED use a VXLAN tunnel to send traffic, and two EDs use a VXLAN-DCI tunnel to send traffic. An ED de-encapsulates incoming VXLAN packets and re-encapsulates them before forwarding the packets through a VXLAN or VXLAN-DCI tunnel.
EVPN-DCI dual-homing
As shown in Figure 2, EVPN-DCI dual-homing allows you to deploy two EDs at a data center for high availability and load sharing. To virtualize the redundant EDs into one device, a virtual ED address is configured on them. The redundant EDs use the virtual ED address to establish tunnels with VTEPs and remote EDs.
Figure 2 EVPN-DCI dual-homing
The redundant EDs use their respective IP addresses as the BGP peer addresses to establish BGP EVPN neighbor relationships with VTEPs and remote EDs. The VTEPs and remote EDs send traffic destined for the virtual ED address to both of the redundant EDs through the ECMP routes provided by the underlay network.
The redundant EDs communicate with remote data centers through the transport network. Devices in the dual-homed data center are unaware of the transport network. When the transport-side link fails on one of the redundant EDs, traffic destined for remote data centers is still sent to that ED. To resolve this issue, Monitor Link is used together with EVPN-DCI dual-homing. On each redundant ED, the transport-facing physical interface is associated with the loopback interface that provides the IP address used for establishing BGP EVPN neighbor relationships. If the transport-side link fails on a redundant ED, the loopback interface is placed in down state, and all traffic is forwarded by the other redundant ED. For more information about Monitor Link, see High Availability Configuration Guide.
For link redundancy, deploy multiple RRs on the spine nodes in a data center, and connect each redundant ED to the transport network through multiple links.
Restrictions and guidelines: EVPN-DCI configuration
On an ED, make sure the VSI interfaces configured with L3 VXLAN IDs use the same MAC address. To modify the MAC address of a VSI interface, use the mac-address command.
EVPN-DCI tasks at a glance
To configure EVPN-DCI, perform the following tasks on EDs:
1.     Enabling DCI
2.     Enabling route nexthop replacement and route router MAC replacement
3.     (Optional.) Configuring VXLAN mapping
Perform this task to provide Layer 2 connectivity for a tenant subnet that uses different VXLAN IDs in multiple data centers.
4.     Configuring the BGP EVPN address family and the BGP VPNv4 address family to exchange routes
You must perform this task if data centers are interconnected through an MPLS L3VPN network.
5.     (Optional.) Configuring EVPN-DCI dual-homing
Prerequisites for EVPN-DCI
Before you configure EVPN-DCI, complete basic EVPN configuration for each data center. For more information about basic EVPN configuration, see "Configuring EVPN VXLAN."
Enabling DCI
For EDs to automatically establish VXLAN-DCI tunnels, you must enable DCI on the Layer 3 interfaces or subinterfaces that interconnect the EDs.
An ED establishes VXLAN-DCI tunnels based on BGP EVPN routes. If DCI is disabled on the outgoing interfaces to remote sites, EDs cannot establish VXLAN-DCI tunnels.
2.     Enter interface or subinterface view.
3.     Enable DCI.
dci enable
By default, DCI is disabled on an interface.
Configuring an ED to modify BGP EVPN routes
2.     Configure a global router ID.
router id router-id
By default, no global router ID is configured.
3.     Enable a BGP instance and enter BGP instance view.
By default, BGP is disabled, and no BGP instances exist.
4.     Specify local VTEPs and remote EDs as BGP peers.
5.     Create the BGP EVPN address family and enter BGP EVPN address family view.
address-family l2vpn evpn
6.     Enable BGP to exchange BGP EVPN routes with a peer or peer group.
By default, BGP does not exchange BGP EVPN routes with peers.
7.     Set the local router as the next hop for routes advertised to a peer or peer group.
The default settings for this command are as follows:
¡     BGP sets the local router as the next hop for all routes advertised to an EBGP peer or peer group.
¡     BGP does not modify the next hop for EBGP routes advertised to an IBGP peer or peer group.
The peers specified in this task must be VTEPs in the local data center.
8.     Enable route router MAC replacement for a peer or peer group.
peer { group-name | ipv4-address [ mask-length ] } router-mac-local
By default, the device does not modify the router MAC address of routes before advertising the routes.
This command enables the device to use its router MAC address to replace the router MAC address of routes received from and advertised to a peer or peer group.
The peers specified in this task must be remote EDs.
Enabling an ED to replace the L3 VXLAN ID, RD, and route targets of BGP EVPN routes
In an EVPN-DCI network, use this feature to hide the L3 VXLAN IDs of data centers or enable communication between data centers that use different L3 VXLAN IDs or route targets.
After you enable this feature on an ED, the ED performs the following operations after receiving BGP EVPN routes:
1.     Matches the route targets of the routes with the import route targets of local VPN instances.
2.     Replaces the L3 VXLAN ID, RD, and route targets of the routes with those of the matching local VPN instance.
3.     Advertises the routes to a VTEP or remote ED.
After you execute the peer re-originated command, the ED advertises only reoriginated BGP EVPN routes. For the ED to advertise both original and reoriginated BGP EVPN routes, execute the peer advertise original-route command.
An ED configured with the peer re-originated and peer advertise original-route commands advertises both original and reoriginated BGP EVPN routes. For the ED to advertise only original BGP EVPN routes, execute the peer suppress re-originated command on the ED.
If the RD of a received BGP EVPN route is identical to the RD of the matching local VPN instance, an ED does not replace the L3 VXLAN ID and route targets of the route or reoriginate the route. As a result, the ED does not advertise the route. As a best practice, assign unique RDs to VPN instances on different EVPN gateways and EDs when you use this feature.
3.     Enter BGP EVPN address family view.
4.     Replace the L3 VXLAN ID, RD, and route targets (optional) of received BGP EVPN routes.
peer { group-name | ipv4-address [ mask-length ] } re-originated [ ip-prefix | mac-ip ] [ replace-rt ]
By default, the device does not modify the BGP EVPN routes that are received from peers or peer groups.
5.     (Optional.) Enable the device to advertise original BGP EVPN routes together with the reoriginated BGP EVPN routes after the peer re-originated command is executed.
peer { group-name | ipv4-address [ mask-length ] } advertise original-route
By default, the device advertises only reoriginated BGP EVPN routes to peers and peer groups after the peer re-originated command is executed.
6.     (Optional.) Suppress advertisement of reoriginated BGP EVPN routes to a peer or peer group.
peer { group-name | ipv4-address [ mask-length ] } suppress re-originated { ip-prefix | mac-ip }
By default, the device advertises reoriginated BGP EVPN routes to peers and peer groups after the peer re-originated command is executed.
The VXLAN mapping feature provides Layer 2 connectivity for a tenant subnet that uses different VXLAN IDs in multiple data centers.
If you map a local VXLAN to a remote VXLAN on an ED, the ED processes routes as follows:
·     When the ED receives the local VXLAN's MAC/IP advertisement routes from local VTEPs, it performs the following operations:
¡     Adds the routes to the local VXLAN.
¡     Replaces the VXLAN ID of the routes with the remote VXLAN ID and advertises the routes to remote EDs.
·     When the ED receives the remote VXLAN's MAC/IP advertisement routes from a remote data center, it adds the routes to the local VXLAN.
VXLAN mapping includes the following types:
·     Non-intermediate VXLAN mapping—When two data centers use different VXLAN IDs for a subnet, map the local VXLAN to the remote VXLAN on the ED of one data center. For example, for VXLAN 10 of data center 1 to communicate with VXLAN 20 of data center 2, map VXLAN 10 to VXLAN 20 on the ED of data center 1.
·     Intermediate VXLAN mapping—When multiple data centers use different VXLAN IDs for a subnet, map the VXLANs to an intermediate VXLAN on all EDs. For example, data center 1 uses VXLAN 10, data center 2 uses VXLAN 20, and data center 3 uses VXLAN 30. To provide connectivity for the VXLANs, map them to intermediate VXLAN 500 on EDs of the data centers. You must use intermediate VXLAN mapping if more than two data centers use different VXLAN IDs. The intermediate VXLAN can be used only for VXLAN mapping, and it cannot be used for common VXLAN services.
You must create mapped remote VXLANs on the device, create an EVPN instance for each remote VXLAN, and configure RD and route target settings for the EVPN instances.
When you use VXLAN mapping, follow these route target restrictions:
·     EVPN instances and EVPN address family of VPN instances do not have the same export targets.
·     EVPN instances and EVPN address family of the public instance do not have the same export targets.
2.     Enter VSI view.
vsi vsi-name
3.     Enter EVPN instance view.
evpn encapsulation vxlan
4.     Map the local VXLAN to a remote VXLAN.
mapping vni vxlan-id
By default, a local VXLAN is not mapped to any remote VXLAN.
The mapped remote VXLAN ID cannot be the reserved VXLAN ID specified by using the reserved vxlan command. For more information about the reserved vxlan command, see VXLAN Command Reference.
About route exchange
When data centers are interconnected through an MPLS L3VPN network, EVPN EDs also act as MPLS L3VPN PEs. To enable communication between the data centers, you must perform the following tasks on the EDs:
·     Configure both MPLS L3VPN and EVPN.
·     Configure the BGP EVPN address family and the BGP VPNv4 address family to exchange routes.
Figure 3 Data centers interconnected through an MPLS L3VPN network
Enabling BGP VPNv4 route advertisement for the BGP EVPN address family
4.     Enable BGP VPNv4 route advertisement for the BGP EVPN address family.
advertise l3vpn route [ replace-rt ][ advertise-policy policy-name ]
By default, BGP VPNv4 routes are not advertised through the BGP EVPN address family.
After you execute this command, the device advertises BGP VPNv4 routes as IP prefix advertisement routes through the BGP EVPN address family.
Enabling BGP EVPN route advertisement for the BGP VPNv4 address family
3.     Enter BGP VPNv4 address family view.
address-family vpnv4
4.     Enable BGP EVPN route advertisement for the BGP VPNv4 address family.
advertise evpn route [ replace-rt ][ advertise-policy policy-name ]
By default, BGP EVPN routes are not advertised through the BGP VPNv4 address family.
After you execute this command, the device advertises IP prefix advertisement routes and MAC/IP advertisement routes that contain host route information through the BGP VPNv4 address family.
For high availability and load sharing, you can deploy two EDs at a data center. To virtualize the redundant EDs into one device, you must configure the same virtual ED address on them.
Do not configure a virtual ED address on the only ED of a data center.
On a redundant ED, the virtual ED address must be the IP address of a loopback interface, and it cannot be the BGP peer IP address of the ED.
Redundant EDs cannot provide access service for local VMs. They can act only as EDs. For correct communication, do not redistribute external routes on only one of the redundant EDs. However, you can redistribute the same external routes on both EDs.
2.     Configure a virtual ED address.
evpn edge group group-ip
By default, no virtual ED address is configured.
EVPN-DCI configuration examples (on routers)
Example: Configuring a basic EVPN-DCI network
As shown in Figure 4:
·     Configure VXLAN 10 on Router A through Router D to provide connectivity for the VMs in the data centers.
·     Configure Router A and Router D as VTEPs, and configure Router B and Router C as EDs.
Figure 4 Network diagram
1.     Configure IP addresses and unicast routing settings:
# Assign IP addresses to the interfaces, as shown in Figure 4. (Details not shown.)
# Configure OSPF on the transport network for the routers to reach one another. (Details not shown.)
2.     Configure Router A:
# Enable L2VPN.
[RouterA] l2vpn enable
# Disable remote MAC address learning.
[RouterA] vxlan tunnel mac-learning disable
# Create VXLAN 10 on VSI vpna.
[RouterA] vsi vpna
[RouterA-vsi-vpna] vxlan 10
[RouterA-vsi-vpna-vxlan-10] quit
# Create an EVPN instance on VSI vpna. Configure the router to automatically generate an RD, and manually configure a route target for the EVPN instance.
[RouterA-vsi-vpna] evpn encapsulation vxlan
[RouterA-vsi-vpna-evpn-vxlan] route-distinguisher auto
[RouterA-vsi-vpna-evpn-vxlan] vpn-target 123:456
[RouterA-vsi-vpna-evpn-vxlan] quit
[RouterA-vsi-vpna] quit
# Configure BGP to advertise BGP EVPN routes.
[RouterA] bgp 100
[RouterA-bgp-default] peer 2.2.2.2 as-number 100
[RouterA-bgp-default] peer 2.2.2.2 connect-interface loopback 0
[RouterA-bgp-default] address-family l2vpn evpn
[RouterA-bgp-default-evpn] peer 2.2.2.2 enable
[RouterA-bgp-default-evpn] quit
[RouterA-bgp-default] quit
# Map site-facing interface GigabitEthernet 1/0/1 to VSI vpna.
[RouterA-GigabitEthernet1/0/1] xconnect vsi vpna
3.     Configure Router B:
# Enable L2VPN.
<RouterB> system-view
[RouterB] l2vpn enable
[RouterB] vxlan tunnel mac-learning disable
# Enable DCI on the Layer 3 interface that connects Router B to Router C for the routers to establish a VXLAN-DCI tunnel.
[RouterB-GigabitEthernet1/0/2] dci enable
[RouterB] vsi vpna
[RouterB-vsi-vpna] vxlan 10
[RouterB-vsi-vpna-vxlan-10] quit
[RouterB-vsi-vpna] evpn encapsulation vxlan
[RouterB-vsi-vpna-evpn-vxlan] route-distinguisher auto
[RouterB-vsi-vpna-evpn-vxlan] vpn-target 123:456
[RouterB-vsi-vpna-evpn-vxlan] quit
[RouterB-vsi-vpna] quit
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Router A, and enable router MAC replacement for routes advertised to and received from Router C.
[RouterB] bgp 100
[RouterB-bgp-default] peer 3.3.3.3 as-number 200
[RouterB-bgp-default] peer 3.3.3.3 connect-interface loopback 0
[RouterB-bgp-default] peer 3.3.3.3 ebgp-max-hop 64
[RouterB-bgp-default] peer 1.1.1.1 as-number 100
[RouterB-bgp-default] peer 1.1.1.1 connect-interface loopback 0
[RouterB-bgp-default] address-family l2vpn evpn
[RouterB-bgp-default-evpn] peer 3.3.3.3 enable
[RouterB-bgp-default-evpn] peer 3.3.3.3 router-mac-local
[RouterB-bgp-default-evpn] peer 1.1.1.1 enable
[RouterB-bgp-default-evpn] peer 1.1.1.1 next-hop-local
[RouterB-bgp-default-evpn] quit
[RouterB-bgp-default] quit
4.     Configure Router C:
# Enable L2VPN.
<RouterC> system-view
[RouterC] l2vpn enable
[RouterC] vxlan tunnel mac-learning disable
# Enable DCI on the Layer 3 interface that connects Router C to Router B for the routers to establish a VXLAN-DCI tunnel.
[RouterC-GigabitEthernet1/0/1] dci enable
[RouterC] vsi vpna
[RouterC-vsi-vpna] vxlan 10
[RouterC-vsi-vpna-vxlan-10] quit
[RouterC-vsi-vpna] evpn encapsulation vxlan
[RouterC-vsi-vpna-evpn-vxlan] route-distinguisher auto
[RouterC-vsi-vpna-evpn-vxlan] vpn-target 123:456
[RouterC-vsi-vpna-evpn-vxlan] quit
[RouterC-vsi-vpna] quit
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Router D, and enable router MAC replacement for routes advertised to and received from Router B.
[RouterC] bgp 200
[RouterC-bgp-default] peer 2.2.2.2 as-number 100
[RouterC-bgp-default] peer 2.2.2.2 connect-interface loopback 0
[RouterC-bgp-default] peer 2.2.2.2 ebgp-max-hop 64
[RouterC-bgp-default] peer 4.4.4.4 as-number 200
[RouterC-bgp-default] peer 4.4.4.4 connect-interface loopback 0
[RouterC-bgp-default] address-family l2vpn evpn
[RouterC-bgp-default-evpn] peer 2.2.2.2 enable
[RouterC-bgp-default-evpn] peer 2.2.2.2 router-mac-local
[RouterC-bgp-default-evpn] peer 4.4.4.4 enable
[RouterC-bgp-default-evpn] peer 4.4.4.4 next-hop-local
[RouterC-bgp-default-evpn] quit
[RouterC-bgp-default] quit
5.     Configure Router D:
# Enable L2VPN.
<RouterD> system-view
[RouterD] l2vpn enable
[RouterD] vxlan tunnel mac-learning disable
[RouterD] vsi vpna
[RouterD-vsi-vpna] vxlan 10
[RouterD-vsi-vpna-vxlan-10] quit
[RouterD-vsi-vpna] evpn encapsulation vxlan
[RouterD-vsi-vpna-evpn-vxlan] route-distinguisher auto
[RouterD-vsi-vpna-evpn-vxlan] vpn-target 123:456
[RouterD-vsi-vpna-evpn-vxlan] quit
[RouterD-vsi-vpna] quit
[RouterD] bgp 200
[RouterD-bgp-default] peer 3.3.3.3 as-number 200
[RouterD-bgp-default] peer 3.3.3.3 connect-interface loopback 0
[RouterD-bgp-default] address-family l2vpn evpn
[RouterD-bgp-default-evpn] peer 3.3.3.3 enable
[RouterD-bgp-default-evpn] quit
[RouterD-bgp-default] quit
[RouterD-GigabitEthernet1/0/1] xconnect vsi vpna
[RouterD-GigabitEthernet1/0/1] quit
1.     Verify the configuration on EDs. (This example uses Router B.)
# Verify that the ED has discovered Router A and Router C through IMET routes and has established VXLAN and VXLAN-DCI tunnels to the routers.
[RouterB] display evpn auto-discovery imet
Total number of automatically discovered peers: 3
VSI name: vpna
RD                    PE_address      Tunnel_address  Tunnel mode VXLAN ID
1:10                  1.1.1.1         1.1.1.1         VXLAN       10
1:10                  3.3.3.3         3.3.3.3         VXLAN-DCI   10
# Verify that the VXLAN and VXLAN-DCI tunnels on the ED are up.
[RouterB] display interface tunnel
Tunnel0
Current state: UP
Line protocol state: UP
Bandwidth: 64 kbps
Maximum transmission unit: 64000
Tunnel source 2.2.2.2, destination 1.1.1.1
Tunnel1
Current state: UP
Bandwidth: 64 kbps
Tunnel source 2.2.2.2, destination 3.3.3.3
Tunnel protocol/transport UDP_VXLAN-DCI/IP
# Verify that the VXLAN and VXLAN-DCI tunnels have been assigned to the VXLAN.
[RouterB] display l2vpn vsi name vpna verbose
VSI Name: vpna
  VSI Index               : 0
  VSI State               : Up
  MTU                     : 1500
  Bandwidth               : Unlimited
  Broadcast Restrain      : -
  Multicast Restrain      : -
  Unknown Unicast Restrain: -
  MAC Table Limit         : -
  Drop Unknown            : Disabled
  PW Redundancy           : Slave
  Service Class           : -
  Statistics              : Disabled
  VXLAN ID                : 10
  Tunnels:
    Tunnel Name          Link ID    State    Type        Flood proxy
    Tunnel0              0x5000000  UP       Auto        Disabled
    Tunnel1              0x5000001  UP       Auto        Disabled
# Verify that the ED has generated EVPN MAC address entries for the VMs.
[RouterB] display evpn route mac
Flags: D - Dynamic   B - BGP   G - Gateway   L - Local active   M - Mapping
VSI name: vpna
MAC address     Link ID/Name    Flags   Next hop
0001-0001-0011  Tunnel0         B       1.1.1.1
0001-0001-0033  Tunnel1         B       3.3.3.3
2.     Verify that VM 1 and VM 2 can communicate. (Details not shown.)
Example: Configuring EVPN-DCI intermediate VXLAN mapping
As shown in Figure 5:
·     Configure VXLAN 10 on VTEP Router A and ED Router B, and configure VXLAN 30 on VTEP Router D and ED Router C.
·     Configure intermediate VXLAN mapping for VXLAN 10 and VXLAN 30 to have Layer 2 connectivity:
¡     Map VXLAN 10 to intermediate VXLAN 500 on Router B.
¡     Map VXLAN 30 to intermediate VXLAN 500 on Router C.
Figure 5 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 5. (Details not shown.)
# Enable L2VPN.
[RouterA] vsi vpna
# Create an EVPN instance on VSI vpna. Configure the router to automatically generate an RD and a route target for the EVPN instance.
[RouterA-vsi-vpna-evpn-vxlan] vpn-target auto
[RouterA] bgp 100
# Enable L2VPN.
[RouterB] vsi vpna
[RouterB-vsi-vpna-evpn-vxlan] vpn-target auto
# Map local VXLAN 10 to intermediate VXLAN 500.
[RouterB-vsi-vpna-evpn-vxlan] mapping vni 500
# Create VXLAN 500 on VSI vpnb. The router will replace the VXLAN ID of VXLAN 10's traffic with VXLAN ID 500 when performing Layer 2 forwarding.
[RouterB] vsi vpnb
[RouterB-vsi-vpnb] vxlan 500
[RouterB-vsi-vpnb-vxlan-500] quit
# Create an EVPN instance on VSI vpnb. Configure the router to automatically generate an RD, and manually configure a route target for the EVPN instance.
[RouterB-vsi-vpnb] evpn encapsulation vxlan
[RouterB-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[RouterB-vsi-vpnb-evpn-vxlan] vpn-target 123:456
[RouterB-vsi-vpnb-evpn-vxlan] quit
[RouterB-vsi-vpnb] quit
[RouterB] bgp 100
# Enable L2VPN.
# Create VXLAN 30 on VSI vpna.
[RouterC] vsi vpna
[RouterC-vsi-vpna] vxlan 30
[RouterC-vsi-vpna-vxlan-30] quit
[RouterC-vsi-vpna-evpn-vxlan] vpn-target auto
# Map local VXLAN 30 to intermediate VXLAN 500.
[RouterC-vsi-vpna-evpn-vxlan] mapping vni 500
# Create VXLAN 500 on VSI vpnb. The router will replace the VXLAN ID of VXLAN 30's traffic with VXLAN ID 500 when performing Layer 2 forwarding.
[RouterC] vsi vpnb
[RouterC-vsi-vpnb] vxlan 500
[RouterC-vsi-vpnb-vxlan-500] quit
[RouterC-vsi-vpnb] evpn encapsulation vxlan
[RouterC-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[RouterC-vsi-vpnb-evpn-vxlan] vpn-target 123:456
[RouterC-vsi-vpnb-evpn-vxlan] quit
[RouterC-vsi-vpnb] quit
[RouterC] bgp 200
# Enable L2VPN.
[RouterD] vsi vpna
[RouterD-vsi-vpna] vxlan 30
[RouterD-vsi-vpna-vxlan-30] quit
[RouterD-vsi-vpna-evpn-vxlan] vpn-target auto
[RouterD] bgp 200
Total number of automatically discovered peers: 2
VSI name: vpna
1:500                 3.3.3.3         3.3.3.3         VXLAN-DCI   500
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel1
Current state: UP
Bandwidth: 64 kbps
# Verify that the VXLAN and VXLAN-DCI tunnels have been assigned to VXLAN 10, and that no tunnels are assigned to intermediate VXLAN 500.
[RouterB] display l2vpn vsi verbose
VSI Name: vpna
  VSI Index               : 0
  VSI State               : Up
  MAC Table Limit         : -
  Service Class           : -
  VXLAN ID                : 10
  Tunnels:
VSI Name: vpnb
  VSI Index               : 1
  VSI State               : Down
  MAC Table Limit         : -
  Service Class           : -
  VXLAN ID                : 500
# Verify that the ED has generated EVPN MAC address entries for the VMs, and the remote MAC address entry has the M flag.
VSI name: vpna
0001-0001-0033  Tunnel1         BM      3.3.3.3
Example: Configuring EVPN-DCI Layer 3 communication
As shown in Figure 6:
·     Configure VXLAN 10 for data center 1, and configure VXLAN 20 for data center 2.
·     Configure Router A and Router D as distributed EVPN gateways to perform Layer 3 forwarding between VXLAN 10 and VXLAN 20.
·     Configure Router B and Router C as EDs.
Figure 6 Network diagram
# On VM 1, specify 10.1.1.1 as the gateway address. On VM 2, specify 10.1.2.1 as the gateway address. (Details not shown.)
# Assign IP addresses to interfaces, as shown in Figure 6. (Details not shown.)
# Enable L2VPN.
# Disable remote MAC address learning and remote ARP learning.
[RouterA] vxlan tunnel arp-learning disable
[RouterA] vsi vpna
[RouterA] bgp 100
# Configure RD and route target settings for VPN instance vpn1.
[RouterA] ip vpn-instance vpn1
[RouterA-vpn-instance-vpn1] route-distinguisher 1:1
[RouterA-vpn-instance-vpn1] address-family ipv4
[RouterA-vpn-ipv4-vpn1] vpn-target 2:2
[RouterA-vpn-ipv4-vpn1] quit
[RouterA-vpn-instance-vpn1] address-family evpn
[RouterA-vpn-evpn-vpn1] vpn-target 1:1
[RouterA-vpn-evpn-vpn1] quit
[RouterA-vpn-instance-vpn1] quit
# Configure VSI-interface 1 as a distributed gateway.
[RouterA] interface vsi-interface 1
[RouterA-Vsi-interface1] ip binding vpn-instance vpn1
[RouterA-Vsi-interface1] ip address 10.1.1.1 255.255.255.0
[RouterA-Vsi-interface1] mac-address 1-1-1
[RouterA-Vsi-interface1] distributed-gateway local
[RouterA-Vsi-interface1] quit
# Create VSI-interface 2. Associate VSI-interface 2 with VPN instance vpn1, and configure the L3 VXLAN ID as 1000 for the VPN instance.
[RouterA] interface vsi-interface 2
[RouterA-Vsi-interface2] ip binding vpn-instance vpn1
[RouterA-Vsi-interface2] l3-vni 1000
[RouterA-Vsi-interface2] quit
# Specify VSI-interface 1 as the gateway interface for VSI vpna.
[RouterA] vsi vpna
[RouterA-vsi-vpna] gateway vsi-interface 1
# Enable L2VPN.
[RouterB] vxlan tunnel arp-learning disable
[RouterB] bgp 100
[RouterB] ip vpn-instance vpn1
[RouterB-vpn-instance-vpn1] route-distinguisher 1:2
[RouterB-vpn-instance-vpn1] address-family ipv4
[RouterB-vpn-ipv4-vpn1] vpn-target 2:2
[RouterB-vpn-ipv4-vpn1] quit
[RouterB-vpn-instance-vpn1] address-family evpn
[RouterB-vpn-evpn-vpn1] vpn-target 1:1
[RouterB-vpn-evpn-vpn1] quit
[RouterB-vpn-instance-vpn1] quit
[RouterB] interface vsi-interface 2
[RouterB-Vsi-interface2] ip binding vpn-instance vpn1
[RouterB-Vsi-interface2] l3-vni 1000
[RouterB-Vsi-interface2] quit
# Enable L2VPN.
[RouterC] vxlan tunnel arp-learning disable
# Enable DCI on the Layer 3 interface that connects Router C to Router B For the routers to establish a VXLAN-DCI tunnel.
[RouterC] bgp 200
[RouterC] ip vpn-instance vpn1
[RouterC-vpn-instance-vpn1] route-distinguisher 1:3
[RouterC-vpn-instance-vpn1] address-family ipv4
[RouterC-vpn-ipv4-vpn1] vpn-target 2:2
[RouterC-vpn-ipv4-vpn1] quit
[RouterC-vpn-instance-vpn1] address-family evpn
[RouterC-vpn-evpn-vpn1] vpn-target 1:1
[RouterC-vpn-evpn-vpn1] quit
[RouterC-vpn-instance-vpn1] quit
[RouterC] interface vsi-interface 2
[RouterC-Vsi-interface2] ip binding vpn-instance vpn1
[RouterC-Vsi-interface2] l3-vni 1000
[RouterC-Vsi-interface2] quit
# Enable L2VPN.
[RouterD] vxlan tunnel arp-learning disable
# Create an EVPN instance on VSI vpnb. Configure the router to automatically generate an RD and a route target for the EVPN instance.
[RouterD] vsi vpnb
[RouterD-vsi-vpnb] evpn encapsulation vxlan
[RouterD-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[RouterD-vsi-vpnb-evpn-vxlan] vpn-target auto
[RouterD-vsi-vpnb-evpn-vxlan] quit
# Create VXLAN 20 on VSI vpnb.
[RouterD-vsi-vpnb] vxlan 20
[RouterD-vsi-vpnb-vxlan-20] quit
[RouterD-vsi-vpnb] quit
[RouterD] bgp 200
# Map site-facing interface GigabitEthernet 1/0/1 to VSI vpnb.
[RouterD-GigabitEthernet1/0/1] xconnect vsi vpnb
[RouterD] ip vpn-instance vpn1
[RouterD-vpn-instance-vpn1] route-distinguisher 1:4
[RouterD-vpn-instance-vpn1] address-family ipv4
[RouterD-vpn-ipv4-vpn1] vpn-target 2:2
[RouterD-vpn-ipv4-vpn1] quit
[RouterD-vpn-instance-vpn1] address-family evpn
[RouterD-vpn-evpn-vpn1] vpn-target 1:1
[RouterD-vpn-evpn-vpn1] quit
[RouterD-vpn-instance-vpn1] quit
[RouterD] interface vsi-interface 1
[RouterD-Vsi-interface1] ip binding vpn-instance vpn1
[RouterD-Vsi-interface1] ip address 10.1.2.1 255.255.255.0
[RouterD-Vsi-interface1] mac-address 1-2-1
[RouterD-Vsi-interface1] distributed-gateway local
[RouterD-Vsi-interface1] quit
[RouterD] interface vsi-interface 2
[RouterD-Vsi-interface2] ip binding vpn-instance vpn1
[RouterD-Vsi-interface2] l3-vni 1000
[RouterD-Vsi-interface2] quit
# Specify VSI-interface 1 as the gateway interface for VSI vpnb.
[RouterD] vsi vpnb
[RouterD-vsi-vpnb] gateway vsi-interface 1
# Verify that the ED has discovered Router A and Router C through MAC/IP advertisement routes and IP prefix advertisement routes, and has established VXLAN and VXLAN-DCI tunnels to the routers.
[RouterB] display evpn auto-discovery macip-prefix
Destination IP  Source IP       L3VNI           Tunnel mode OutgoingInterface
1.1.1.1         2.2.2.2         1000            VXLAN       Vsi-interface2
3.3.3.3         2.2.2.2         1000            VXLAN-DCI   Vsi-interface2
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel1
Current state: UP
Bandwidth: 64 kbps
# Verify that the ED has EVPN ARP entries and EVPN routes for the VMs.
[RouterB] display arp vpn-instance vpn1
  Type: S-Static   D-Dynamic   O-Openflow   R-Rule   M-Multiport  I-Invalid
IP address      MAC address    VLAN/VSI name Interface/Link ID        Aging Type
1.1.1.1         0031-1900-0000 Auto_L3VNI100 Tunnel0                  --    R
                               0_2
3.3.3.3         0031-3900-0000 Auto_L3VNI100 Tunnel1                  --    R
                               0_2
[RouterB] display ip routing-table vpn-instance vpn1
Destinations : 4        Routes : 4
10.1.1.0/24        BGP     255 0           1.1.1.1         Vsi2
10.1.1.11/32       BGP     255 0           1.1.1.1         Vsi2
10.1.2.0/24        BGP     255 0           3.3.3.3         Vsi2
10.1.2.22/32       BGP     255 0           3.3.3.3         Vsi2
Example: Configuring EVPN-DCI dual-homing
As shown in Figure 7:
·     Configure Router A and Router G as distributed EVPN gateways to perform Layer 3 forwarding between VXLAN 10 and VXLAN 20.
·     Configure Router C and Router D as EDs of data center 1, and configure Router F as the ED of data center 2.
·     Configure Router B as an RR.
Figure 7 Network diagram
# On VM 1, specify 100.1.1.1 as the gateway address. On VM 2, specify 100.1.2.1 as the gateway address. (Details not shown.)
# Assign IP addresses to the interfaces, as shown in Figure 7. (Details not shown.)
# Configure OSPF for the routers to reach one another. (Details not shown.)
# Enable L2VPN.
[RouterA] vsi vpna
[RouterA] bgp 100
# Map GigabitEthernet 1/0/1 to VSI vpna.
[RouterA-Vsi-interface1] ip address 100.1.1.1 255.255.255.0
[RouterA] vsi vpna
3.     Configure Router B as an RR.
[RouterB] bgp 100
[RouterB-bgp-default] group evpn internal
[RouterB-bgp-default] peer evpn connect-interface loopback 0
[RouterB-bgp-default] peer 1.1.1.1 group evpn
[RouterB-bgp-default] peer 3.3.3.3 group evpn
[RouterB-bgp-default] peer 4.4.4.4 group evpn
[RouterB-bgp-default-evpn] undo policy vpn-target
[RouterB-bgp-default-evpn] peer evpn enable
[RouterB-bgp-default-evpn] peer evpn reflect-client
# Enable L2VPN.
# Enable DCI on the Layer 3 interface that connects Router C to Router E for automatic VXLAN-DCI tunnel establishment.
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Router B, and enable router MAC replacement for routes advertised to and received from Router F.
[RouterC] bgp 100
[RouterC-bgp-default] peer 6.6.6.6 as-number 200
[RouterC-bgp-default] peer 6.6.6.6 connect-interface loopback 0
[RouterC-bgp-default] peer 6.6.6.6 ebgp-max-hop 64
[RouterC-bgp-default-evpn] peer 6.6.6.6 enable
[RouterC-bgp-default-evpn] peer 6.6.6.6 router-mac-local
[RouterC-bgp-default-evpn] peer 2.2.2.2 next-hop-local
[RouterC-vpn-instance-vpn1] route-distinguisher 1:2
[RouterC-Vsi-interface2] mac-address 1-2-3
# Configure 1.2.3.4 as the virtual ED address, and assign the IP address to Loopback 2. Configure OSPF to advertise the virtual ED address.
[RouterC] evpn edge group 1.2.3.4
[RouterC] interface loopback 2
[RouterC-LoopBack2] ip address 1.2.3.4 32
[RouterC-LoopBack2] quit
[RouterC] ospf
[RouterC-ospf-1] area 0
[RouterC-ospf-1-area-0.0.0.0] network 1.2.3.4 0.0.0.0
[RouterC-ospf-1] quit
# Configure monitor link group 1 to associate GigabitEthernet 1/0/1 with Loopback 0. Set the switchover delay for the downlink interface to 90 seconds.
[RouterC] undo monitor-link disable
[RouterC] monitor-link group 1
[RouterC-mtlk-group1] port gigabitethernet 1/0/1 uplink
[RouterC-mtlk-group1] port loopback 0 downlink
[RouterC-mtlk-group1] downlink up-delay 90
[RouterC-mtlk-group1] quit
# Enable L2VPN.
# Enable DCI on the Layer 3 interface that connects Router D to Router E for automatic VXLAN-DCI tunnel establishment.
[RouterD-GigabitEthernet1/0/1] dci enable
[RouterD] bgp 100
[RouterD-bgp-default] peer 6.6.6.6 as-number 200
[RouterD-bgp-default] peer 6.6.6.6 connect-interface loopback 0
[RouterD-bgp-default] peer 6.6.6.6 ebgp-max-hop 64
[RouterD-bgp-default] peer 2.2.2.2 as-number 100
[RouterD-bgp-default] peer 2.2.2.2 connect-interface loopback 0
[RouterD-bgp-default-evpn] peer 6.6.6.6 enable
[RouterD-bgp-default-evpn] peer 6.6.6.6 router-mac-local
[RouterD-bgp-default-evpn] peer 2.2.2.2 enable
[RouterD-bgp-default-evpn] peer 2.2.2.2 next-hop-local
[RouterD-vpn-instance-vpn1] route-distinguisher 1:2
[RouterD-Vsi-interface2] mac-address 1-2-3
[RouterD] evpn edge group 1.2.3.4
[RouterD] interface loopback 2
[RouterD-LoopBack2] ip address 1.2.3.4 32
[RouterD-LoopBack2] quit
[RouterD] ospf
[RouterD-ospf-1] area 0
[RouterD-ospf-1-area-0.0.0.0] network 1.2.3.4 0.0.0.0
[RouterD-ospf-1-area-0.0.0.0] quit
[RouterD-ospf-1] quit
[RouterD] undo monitor-link disable
[RouterD] monitor-link group 1
[RouterD-mtlk-group1] port gigabitethernet 1/0/1 uplink
[RouterD-mtlk-group1] port loopback 0 downlink
[RouterD-mtlk-group1] downlink up-delay 90
[RouterD-mtlk-group1] quit
6.     Configure Router F:
# Enable L2VPN.
<RouterF> system-view
[RouterF] l2vpn enable
[RouterF] vxlan tunnel mac-learning disable
[RouterF] vxlan tunnel arp-learning disable
# Enable DCI on the Layer 3 interface that connects Router F to Router E for automatic VXLAN-DCI tunnel establishment.
[RouterF] interface gigabitethernet 1/0/1
[RouterF-GigabitEthernet1/0/1] dci enable
[RouterF-GigabitEthernet1/0/1] quit
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Router G, and enable router MAC replacement for routes advertised to and received from Router C and Router D.
[RouterF] bgp 200
[RouterF-bgp-default] peer 3.3.3.3 as-number 100
[RouterF-bgp-default] peer 3.3.3.3 connect-interface loopback 0
[RouterF-bgp-default] peer 3.3.3.3 ebgp-max-hop 64
[RouterF-bgp-default] peer 4.4.4.4 as-number 100
[RouterF-bgp-default] peer 4.4.4.4 connect-interface loopback 0
[RouterF-bgp-default] peer 4.4.4.4 ebgp-max-hop 64
[RouterF-bgp-default] peer 7.7.7.7 as-number 200
[RouterF-bgp-default] peer 7.7.7.7 connect-interface loopback 0
[RouterF-bgp-default] address-family l2vpn evpn
[RouterF-bgp-default-evpn] peer 3.3.3.3 enable
[RouterF-bgp-default-evpn] peer 3.3.3.3 router-mac-local
[RouterF-bgp-default-evpn] peer 4.4.4.4 enable
[RouterF-bgp-default-evpn] peer 4.4.4.4 router-mac-local
[RouterF-bgp-default-evpn] peer 7.7.7.7 enable
[RouterF-bgp-default-evpn] peer 7.7.7.7 next-hop-local
[RouterF-bgp-default-evpn] quit
[RouterF-bgp-default] quit
[RouterF] ip vpn-instance vpn1
[RouterF-vpn-instance-vpn1] route-distinguisher 1:4
[RouterF-vpn-instance-vpn1] address-family ipv4
[RouterF-vpn-ipv4-vpn1] vpn-target 2:2
[RouterF-vpn-ipv4-vpn1] quit
[RouterF-vpn-instance-vpn1] address-family evpn
[RouterF-vpn-evpn-vpn1] vpn-target 1:1
[RouterF-vpn-evpn-vpn1] quit
[RouterF-vpn-instance-vpn1] quit
[RouterF] interface vsi-interface 2
[RouterF-Vsi-interface2] ip binding vpn-instance vpn1
[RouterF-Vsi-interface2] l3-vni 1000
[RouterF-Vsi-interface2] quit
7.     Configure Router G:
# Enable L2VPN.
<RouterG> system-view
[RouterG] l2vpn enable
[RouterG] vxlan tunnel mac-learning disable
[RouterG] vxlan tunnel arp-learning disable
[RouterG] vsi vpnb
[RouterG-vsi-vpnb] vxlan 20
[RouterG-vsi-vpnb-vxlan-20] quit
[RouterG-vsi-vpnb] evpn encapsulation vxlan
[RouterG-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[RouterG-vsi-vpnb-evpn-vxlan] vpn-target auto
[RouterG-vsi-vpnb-evpn-vxlan] quit
[RouterG-vsi-vpnb] quit
[RouterG] bgp 200
[RouterG-bgp-default] peer 6.6.6.6 as-number 200
[RouterG-bgp-default] peer 6.6.6.6 connect-interface loopback 0
[RouterG-bgp-default] address-family l2vpn evpn
[RouterG-bgp-default-evpn] peer 6.6.6.6 enable
[RouterG-bgp-default-evpn] quit
[RouterG-bgp-default] quit
# Map GigabitEthernet 1/0/1 to VSI vpnb.
[RouterG] interface gigabitethernet 1/0/1
[RouterG-GigabitEthernet1/0/1] xconnect vsi vpnb
[RouterG-GigabitEthernet1/0/1] quit
[RouterG] ip vpn-instance vpn1
[RouterG-vpn-instance-vpn1] route-distinguisher 1:4
[RouterG-vpn-instance-vpn1] address-family ipv4
[RouterG-vpn-ipv4-vpn1] vpn-target 2:2
[RouterG-vpn-ipv4-vpn1] quit
[RouterG-vpn-instance-vpn1] address-family evpn
[RouterG-vpn-evpn-vpn1] vpn-target 1:1
[RouterG-vpn-evpn-vpn1] quit
[RouterG-vpn-instance-vpn1] quit
[RouterG] interface vsi-interface 1
[RouterG-Vsi-interface1] ip binding vpn-instance vpn1
[RouterG-Vsi-interface1] ip address 100.1.2.1 255.255.255.0
[RouterG-Vsi-interface1] mac-address 2-2-2
[RouterG-Vsi-interface1] distributed-gateway local
[RouterG-Vsi-interface1] quit
[RouterG] interface vsi-interface 2
[RouterG-Vsi-interface2] ip binding vpn-instance vpn1
[RouterG-Vsi-interface2] l3-vni 1000
[RouterG-Vsi-interface2] quit
[RouterG] vsi vpnb
[RouterG-vsi-vpnb] gateway vsi-interface 1
1.     Verify the configuration on EDs. (This example uses Router C.)
# Verify that the ED has discovered Router A and Router F through MAC/IP advertisement routes and IP prefix advertisement routes, and has established VXLAN and VXLAN-DCI tunnels to the routers.
[RouterC] display evpn auto-discovery macip-prefix
Destination IP  Source IP       L3VNI           Tunnel mode OutInterface
1.1.1.1         1.2.3.4         1000            VXLAN       Vsi-interface2
6.6.6.6         1.2.3.4         1000            VXLAN-DCI   Vsi-interface2
[RouterC] display interface tunnel
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel source 1.2.3.4, destination 1.1.1.1
Tunnel1
Current state: UP
Bandwidth: 64 kbps
Tunnel source 1.2.3.4, destination 6.6.6.6
# Verify that the ED has ARP entries and routes for the VMs.
[RouterC] display arp vpn-instance vpn1
  Type: S  Type: S-Static   D-Dynamic   O-Openflow   R-Rule   M-Multiport  I-Invalid
                               0_2
6.6.6.6         0031-3900-0000 Auto_L3VNI100 Tunnel1                  --    R
                               0_2
[RouterC] display ip routing-table vpn-instance vpn1
100.1.1.0/24       BGP     255 0           1.1.1.1         Vsi2
100.1.1.10/32      BGP     255 0           1.1.1.1         Vsi2
100.1.2.0/24       BGP     255 0           6.6.6.6         Vsi2
100.1.2.20/32      BGP     255 0           6.6.6.6         Vsi2
2.     Verify the configuration on Router A:
# Verify that the router has discovered the virtual ED through MAC/IP advertisement routes and IP prefix advertisement routes, and has established a VXLAN tunnel to the virtual ED.
[RouterA] display evpn auto-discovery macip-prefix
1.2.3.4         1.1.1.1         1000            VXLAN       Vsi-interface2
# Verify that the VXLAN tunnel on the router is up.
[RouterA] display interface tunnel
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel source 1.1.1.1, destination 1.2.3.4
# Verify that the router has ARP entries and routes for the VMs.
[RouterA] display arp vpn-instance vpn1
1.2.3.4         0031-1900-0001 Auto_L3VNI100 Tunnel0                  --    R
                               0_2
[RouterA] display ip routing-table vpn-instance vpn1
100.1.2.0/24       BGP     255 0           1.2.3.4         Vsi2
100.1.2.10/32      BGP     255 0           1.2.3.4         Vsi2
3.     Verify that VM 1 and VM 2 can communicate when both Router C and Router D are working correctly and when Router C or Router D fails. (Details not shown.)
EVPN-DCI configuration examples (on switches)
As shown in Figure 8:
·     Configure VXLAN 10 on Switch A through Switch D to provide connectivity for the VMs in the data centers.
·     Configure Switch A and Switch D as VTEPs, and configure Switch B and Switch C as EDs.
Figure 8 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 8. (Details not shown.)
# Configure OSPF on the transport network for the switches to reach one another. (Details not shown.)
2.     Configure Switch A:
# Enable L2VPN.
[SwitchA] l2vpn enable
[SwitchA] vxlan tunnel mac-learning disable
[SwitchA] vsi vpna
[SwitchA-vsi-vpna] vxlan 10
# Create an EVPN instance on VSI vpna. Configure the switch to automatically generate an RD, and manually configure a route target for the EVPN instance.
[SwitchA-vsi-vpna] evpn encapsulation vxlan
[SwitchA-vsi-vpna-evpn-vxlan] route-distinguisher auto
[SwitchA-vsi-vpna-evpn-vxlan] vpn-target 123:456
[SwitchA-vsi-vpna-evpn-vxlan] quit
[SwitchA-vsi-vpna] quit
[SwitchA] bgp 100
[SwitchA-bgp-default] peer 2.2.2.2 as-number 100
[SwitchA-bgp-default] peer 2.2.2.2 connect-interface loopback 0
[SwitchA-bgp-default] address-family l2vpn evpn
[SwitchA-bgp-default-evpn] peer 2.2.2.2 enable
[SwitchA-bgp-default-evpn] quit
[SwitchA-bgp-default] quit
# On GigabitEthernet 1/0/1, create Ethernet service instance 1000 to match VLAN 100.
[SwitchA-GigabitEthernet1/0/1] service-instance 1000
[SwitchA-GigabitEthernet1/0/1-srv1000] encapsulation s-vid 100
# Map Ethernet service instance 1000 to VSI vpna.
[SwitchA-GigabitEthernet1/0/1-srv1000] xconnect vsi vpna
[SwitchA-GigabitEthernet1/0/1-srv1000] quit
3.     Configure Switch B:
# Enable L2VPN.
[SwitchB] l2vpn enable
[SwitchB] vxlan tunnel mac-learning disable
# Enable DCI on the Layer 3 interface that connects Switch B to Switch C for the switches to establish a VXLAN-DCI tunnel.
[SwitchB] interface vlan-interface 12
[SwitchB-Vlan-interface12] dci enable
[SwitchB-Vlan-interface12] quit
[SwitchB] vsi vpna
[SwitchB-vsi-vpna] vxlan 10
[SwitchB-vsi-vpna] evpn encapsulation vxlan
[SwitchB-vsi-vpna-evpn-vxlan] route-distinguisher auto
[SwitchB-vsi-vpna-evpn-vxlan] vpn-target 123:456
[SwitchB-vsi-vpna-evpn-vxlan] quit
[SwitchB-vsi-vpna] quit
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Switch A, and enable router MAC replacement for routes advertised to and received from Switch C.
[SwitchB] bgp 100
[SwitchB-bgp-default] peer 3.3.3.3 as-number 200
[SwitchB-bgp-default] peer 3.3.3.3 ebgp-max-hop 64
[SwitchB-bgp-default] peer 1.1.1.1 as-number 100
[SwitchB-bgp-default] peer 1.1.1.1 connect-interface loopback 0
[SwitchB-bgp-default] address-family l2vpn evpn
[SwitchB-bgp-default-evpn] peer 3.3.3.3 enable
[SwitchB-bgp-default-evpn] peer 3.3.3.3 router-mac-local
[SwitchB-bgp-default-evpn] peer 1.1.1.1 enable
[SwitchB-bgp-default-evpn] peer 1.1.1.1 next-hop-local
[SwitchB-bgp-default-evpn] quit
[SwitchB-bgp-default] quit
4.     Configure Switch C:
# Enable L2VPN.
[SwitchC] l2vpn enable
[SwitchC] vxlan tunnel mac-learning disable
# Enable DCI on the Layer 3 interface that connects Switch C to Switch B for the switches to establish a VXLAN-DCI tunnel.
[SwitchC] interface vlan-interface 12
[SwitchC-Vlan-interface12] dci enable
[SwitchC-Vlan-interface12] quit
[SwitchC] vsi vpna
[SwitchC-vsi-vpna] vxlan 10
[SwitchC-vsi-vpna] evpn encapsulation vxlan
[SwitchC-vsi-vpna-evpn-vxlan] route-distinguisher auto
[SwitchC-vsi-vpna-evpn-vxlan] vpn-target 123:456
[SwitchC-vsi-vpna-evpn-vxlan] quit
[SwitchC-vsi-vpna] quit
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Switch D, and enable router MAC replacement for routes advertised to and received from Switch B.
[SwitchC] bgp 200
[SwitchC-bgp-default] peer 2.2.2.2 as-number 100
[SwitchC-bgp-default] peer 2.2.2.2 ebgp-max-hop 64
[SwitchC-bgp-default] peer 4.4.4.4 as-number 200
[SwitchC-bgp-default] peer 4.4.4.4 connect-interface loopback 0
[SwitchC-bgp-default] address-family l2vpn evpn
[SwitchC-bgp-default-evpn] peer 2.2.2.2 enable
[SwitchC-bgp-default-evpn] peer 2.2.2.2 router-mac-local
[SwitchC-bgp-default-evpn] peer 4.4.4.4 enable
[SwitchC-bgp-default-evpn] peer 4.4.4.4 next-hop-local
[SwitchC-bgp-default-evpn] quit
[SwitchC-bgp-default] quit
5.     Configure Switch D:
# Enable L2VPN.
<SwitchD> system-view
[SwitchD] l2vpn enable
[SwitchD] vxlan tunnel mac-learning disable
[SwitchD] vsi vpna
[SwitchD-vsi-vpna] vxlan 10
[SwitchD-vsi-vpna-vxlan-10] quit
[SwitchD-vsi-vpna] evpn encapsulation vxlan
[SwitchD-vsi-vpna-evpn-vxlan] route-distinguisher auto
[SwitchD-vsi-vpna-evpn-vxlan] vpn-target 123:456
[SwitchD-vsi-vpna-evpn-vxlan] quit
[SwitchD-vsi-vpna] quit
[SwitchD] bgp 200
[SwitchD-bgp-default] peer 3.3.3.3 as-number 200
[SwitchD-bgp-default] peer 3.3.3.3 connect-interface loopback 0
[SwitchD-bgp-default] address-family l2vpn evpn
[SwitchD-bgp-default-evpn] peer 3.3.3.3 enable
[SwitchD-bgp-default-evpn] quit
[SwitchD-bgp-default] quit
# On GigabitEthernet 1/0/1, create Ethernet service instance 1000 to match VLAN 200.
[SwitchD] interface gigabitethernet 1/0/1
[SwitchD-GigabitEthernet1/0/1] service-instance 1000
[SwitchD-GigabitEthernet1/0/1-srv1000] encapsulation s-vid 200
[SwitchD-GigabitEthernet1/0/1-srv1000] xconnect vsi vpna
[SwitchD-GigabitEthernet1/0/1-srv1000] quit
1.     Verify the configuration on EDs. (This example uses Switch B.)
# Verify that the ED has discovered Switch A and Switch C through IMET routes and has established VXLAN and VXLAN-DCI tunnels to the switches.
[SwitchB] display evpn auto-discovery imet
VSI name: vpna
[SwitchB] display interface tunnel
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel1
Current state: UP
Bandwidth: 64 kbps
[SwitchB] display l2vpn vsi name vpna verbose
VSI Name: vpna
  VSI Index               : 0
  VSI State               : Up
  MAC Table Limit         : -
  Service Class           : -
  VXLAN ID                : 10
  Tunnels:
[SwitchB] display evpn route mac
VSI name: vpna
As shown in Figure 9:
·     Configure VXLAN 10 on VTEP Switch A and ED Switch B, and configure VXLAN 30 on VTEP Switch D and ED Switch C.
¡     Map VXLAN 10 to intermediate VXLAN 500 on Switch B.
¡     Map VXLAN 30 to intermediate VXLAN 500 on Switch C.
Figure 9 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 9. (Details not shown.)
# Enable L2VPN.
[SwitchA] vsi vpna
# Create an EVPN instance on VSI vpna. Configure the switch to automatically generate an RD and a route target for the EVPN instance.
[SwitchA-vsi-vpna-evpn-vxlan] vpn-target auto
[SwitchA] bgp 100
# Enable L2VPN.
[SwitchB] vsi vpna
[SwitchB-vsi-vpna-evpn-vxlan] vpn-target auto
[SwitchB-vsi-vpna-evpn-vxlan] mapping vni 500
# Create VXLAN 500 on VSI vpnb. The switch will replace the VXLAN ID of VXLAN 10's traffic with VXLAN ID 500 when performing Layer 2 forwarding.
[SwitchB] vsi vpnb
[SwitchB-vsi-vpnb] vxlan 500
[SwitchB-vsi-vpnb-vxlan-500] quit
# Create an EVPN instance on VSI vpnb. Configure the switch to automatically generate an RD, and manually configure a route target for the EVPN instance.
[SwitchB-vsi-vpnb] evpn encapsulation vxlan
[SwitchB-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[SwitchB-vsi-vpnb-evpn-vxlan] vpn-target 123:456
[SwitchB-vsi-vpnb-evpn-vxlan] quit
[SwitchB-vsi-vpnb] quit
[SwitchB] bgp 100
# Enable L2VPN.
[SwitchC] vsi vpna
[SwitchC-vsi-vpna] vxlan 30
[SwitchC-vsi-vpna-vxlan-30] quit
[SwitchC-vsi-vpna-evpn-vxlan] vpn-target auto
[SwitchC-vsi-vpna-evpn-vxlan] mapping vni 500
# Create VXLAN 500 on VSI vpnb. The switch will replace the VXLAN ID of VXLAN 30's traffic with VXLAN ID 500 when performing Layer 2 forwarding.
[SwitchC] vsi vpnb
[SwitchC-vsi-vpnb] vxlan 500
[SwitchC-vsi-vpnb-vxlan-500] quit
[SwitchC-vsi-vpnb] evpn encapsulation vxlan
[SwitchC-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[SwitchC-vsi-vpnb-evpn-vxlan] vpn-target 123:456
[SwitchC-vsi-vpnb-evpn-vxlan] quit
[SwitchC-vsi-vpnb] quit
[SwitchC] bgp 200
# Enable L2VPN.
[SwitchD] vsi vpna
[SwitchD-vsi-vpna] vxlan 30
[SwitchD-vsi-vpna-vxlan-30] quit
[SwitchD-vsi-vpna-evpn-vxlan] vpn-target auto
[SwitchD] bgp 200
VSI name: vpna
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel1
Current state: UP
Bandwidth: 64 kbps
[SwitchB] display l2vpn vsi verbose
VSI Name: vpna
  VSI Index               : 0
  VSI State               : Up
  MAC Table Limit         : -
  Drop Unknown            : -
  Service Class           : -
  VXLAN ID                : 10
  Tunnels:
VSI Name: vpnb
  VSI Index               : 1
  VSI State               : Down
  MAC Table Limit         : -
  Drop Unknown            : -
  Service Class           : -
  VXLAN ID                : 500
VSI name: vpna
As shown in Figure 10:
·     Configure Switch A and Switch D as distributed EVPN gateways to perform Layer 3 forwarding between VXLAN 10 and VXLAN 20.
·     Configure Switch B and Switch C as EDs.
Figure 10 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 10. (Details not shown.)
# Enable L2VPN.
[SwitchA] vxlan tunnel arp-learning disable
[SwitchA] vsi vpna
[SwitchA] bgp 100
[SwitchA] ip vpn-instance vpn1
[SwitchA-vpn-instance-vpn1] route-distinguisher 1:1
[SwitchA-vpn-instance-vpn1] address-family ipv4
[SwitchA-vpn-ipv4-vpn1] vpn-target 2:2
[SwitchA-vpn-ipv4-vpn1] quit
[SwitchA-vpn-instance-vpn1] address-family evpn
[SwitchA-vpn-evpn-vpn1] vpn-target 1:1
[SwitchA-vpn-evpn-vpn1] quit
[SwitchA-vpn-instance-vpn1] quit
[SwitchA] interface vsi-interface 1
[SwitchA-Vsi-interface1] ip binding vpn-instance vpn1
[SwitchA-Vsi-interface1] ip address 10.1.1.1 255.255.255.0
[SwitchA-Vsi-interface1] mac-address 1-1-1
[SwitchA-Vsi-interface1] distributed-gateway local
[SwitchA-Vsi-interface1] quit
[SwitchA] interface vsi-interface 2
[SwitchA-Vsi-interface2] ip binding vpn-instance vpn1
[SwitchA-Vsi-interface2] l3-vni 1000
[SwitchA-Vsi-interface2] quit
[SwitchA] vsi vpna
[SwitchA-vsi-vpna] gateway vsi-interface 1
# Enable L2VPN.
[SwitchB] vxlan tunnel arp-learning disable
[SwitchB] bgp 100
[SwitchB] ip vpn-instance vpn1
[SwitchB-vpn-instance-vpn1] route-distinguisher 1:2
[SwitchB-vpn-instance-vpn1] address-family ipv4
[SwitchB-vpn-ipv4-vpn1] vpn-target 2:2
[SwitchB-vpn-ipv4-vpn1] quit
[SwitchB-vpn-instance-vpn1] address-family evpn
[SwitchB-vpn-evpn-vpn1] vpn-target 1:1
[SwitchB-vpn-evpn-vpn1] quit
[SwitchB-vpn-instance-vpn1] quit
[SwitchB] interface vsi-interface 2
[SwitchB-Vsi-interface2] ip binding vpn-instance vpn1
[SwitchB-Vsi-interface2] l3-vni 1000
[SwitchB-Vsi-interface2] quit
# Enable L2VPN.
[SwitchC] vxlan tunnel arp-learning disable
# Enable DCI on the Layer 3 interface that connects Switch C to Switch B For the switches to establish a VXLAN-DCI tunnel.
[SwitchC] bgp 200
[SwitchC] ip vpn-instance vpn1
[SwitchC-vpn-instance-vpn1] route-distinguisher 1:3
[SwitchC-vpn-instance-vpn1] address-family ipv4
[SwitchC-vpn-ipv4-vpn1] vpn-target 2:2
[SwitchC-vpn-ipv4-vpn1] quit
[SwitchC-vpn-instance-vpn1] address-family evpn
[SwitchC-vpn-evpn-vpn1] vpn-target 1:1
[SwitchC-vpn-evpn-vpn1] quit
[SwitchC-vpn-instance-vpn1] quit
[SwitchC] interface vsi-interface 2
[SwitchC-Vsi-interface2] ip binding vpn-instance vpn1
[SwitchC-Vsi-interface2] l3-vni 1000
[SwitchC-Vsi-interface2] quit
# Enable L2VPN.
[SwitchD] vxlan tunnel arp-learning disable
# Create an EVPN instance on VSI vpnb. Configure the switch to automatically generate an RD and a route target for the EVPN instance.
[SwitchD] vsi vpnb
[SwitchD-vsi-vpnb] evpn encapsulation vxlan
[SwitchD-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[SwitchD-vsi-vpnb-evpn-vxlan] vpn-target auto
[SwitchD-vsi-vpnb-evpn-vxlan] quit
[SwitchD-vsi-vpnb] vxlan 20
[SwitchD-vsi-vpnb-vxlan-20] quit
[SwitchD-vsi-vpnb] quit
[SwitchD] bgp 200
# On GigabitEthernet 1/0/1, create Ethernet service instance 3000 to match VLAN 3.
[SwitchD-GigabitEthernet1/0/1] service-instance 3000
[SwitchD-GigabitEthernet1/0/1-srv3000] encapsulation s-vid 3
# Map Ethernet service instance 3000 to VSI vpnb.
[SwitchD-GigabitEthernet1/0/1-srv3000] xconnect vsi vpnb
[SwitchD-GigabitEthernet1/0/1-srv3000] quit
[SwitchD] ip vpn-instance vpn1
[SwitchD-vpn-instance-vpn1] route-distinguisher 1:4
[SwitchD-vpn-instance-vpn1] address-family ipv4
[SwitchD-vpn-ipv4-vpn1] vpn-target 2:2
[SwitchD-vpn-ipv4-vpn1] quit
[SwitchD-vpn-instance-vpn1] address-family evpn
[SwitchD-vpn-evpn-vpn1] vpn-target 1:1
[SwitchD-vpn-evpn-vpn1] quit
[SwitchD-vpn-instance-vpn1] quit
[SwitchD] interface vsi-interface 1
[SwitchD-Vsi-interface1] ip binding vpn-instance vpn1
[SwitchD-Vsi-interface1] ip address 10.1.2.1 255.255.255.0
[SwitchD-Vsi-interface1] mac-address 1-2-1
[SwitchD-Vsi-interface1] distributed-gateway local
[SwitchD-Vsi-interface1] quit
[SwitchD] interface vsi-interface 2
[SwitchD-Vsi-interface2] ip binding vpn-instance vpn1
[SwitchD-Vsi-interface2] l3-vni 1000
[SwitchD-Vsi-interface2] quit
[SwitchD] vsi vpnb
[SwitchD-vsi-vpnb] gateway vsi-interface 1
# Verify that the ED has discovered Switch A and Switch C through MAC/IP advertisement routes and IP prefix advertisement routes, and has established VXLAN and VXLAN-DCI tunnels to the switches.
[SwitchB] display evpn auto-discovery macip-prefix
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel1
Current state: UP
Bandwidth: 64 kbps
[SwitchB] display arp vpn-instance vpn1
                               0_2
                               0_2
[SwitchB] display ip routing-table vpn-instance vpn1
As shown in Figure 11:
·     Configure Switch A and Switch G as distributed EVPN gateways to perform Layer 3 forwarding between VXLAN 10 and VXLAN 20.
·     Configure Switch C and Switch D as EDs of data center 1, and configure Switch F as the ED of data center 2.
·     Configure Switch B as an RR.
Figure 11 Network diagram
# Assign IP addresses to the interfaces, as shown in Figure 11. (Details not shown.)
# Configure OSPF for the switches to reach one another. (Details not shown.)
# Enable L2VPN.
[SwitchA] vsi vpna
[SwitchA] bgp 100
[SwitchA-Vsi-interface1] ip address 100.1.1.1 255.255.255.0
[SwitchA] vsi vpna
3.     Configure Switch B as an RR.
[SwitchB] bgp 100
[SwitchB-bgp-default] group evpn internal
[SwitchB-bgp-default] peer evpn connect-interface loopback 0
[SwitchB-bgp-default] peer 1.1.1.1 group evpn
[SwitchB-bgp-default] peer 3.3.3.3 group evpn
[SwitchB-bgp-default] peer 4.4.4.4 group evpn
[SwitchB-bgp-default-evpn] undo policy vpn-target
[SwitchB-bgp-default-evpn] peer evpn enable
[SwitchB-bgp-default-evpn] peer evpn reflect-client
# Enable L2VPN.
# Enable DCI on the Layer 3 interface that connects Switch C to Switch E for automatic VXLAN-DCI tunnel establishment.
[SwitchC] interface vlan-interface 13
[SwitchC-Vlan-interface13] dci enable
[SwitchC-Vlan-interface13] quit
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Switch B, and enable router MAC replacement for routes advertised to and received from Switch F.
[SwitchC] bgp 100
[SwitchC-bgp-default] peer 6.6.6.6 as-number 200
[SwitchC-bgp-default] peer 6.6.6.6 connect-interface loopback 0
[SwitchC-bgp-default] peer 6.6.6.6 ebgp-max-hop 64
[SwitchC-bgp-default-evpn] peer 6.6.6.6 enable
[SwitchC-bgp-default-evpn] peer 6.6.6.6 router-mac-local
[SwitchC-bgp-default-evpn] peer 2.2.2.2 next-hop-local
[SwitchC-vpn-instance-vpn1] route-distinguisher 1:2
[SwitchC-Vsi-interface2] mac-address 1-2-3
[SwitchC] evpn edge group 1.2.3.4
[SwitchC] interface loopback 2
[SwitchC-LoopBack2] ip address 1.2.3.4 32
[SwitchC-LoopBack2] quit
[SwitchC] ospf
[SwitchC-ospf-1] area 0
[SwitchC-ospf-1-area-0.0.0.0] network 1.2.3.4 0.0.0.0
[SwitchC-ospf-1] quit
[SwitchC] undo monitor-link disable
[SwitchC] monitor-link group 1
[SwitchC-mtlk-group1] port gigabitethernet 1/0/1 uplink
[SwitchC-mtlk-group1] port loopback 0 downlink
[SwitchC-mtlk-group1] downlink up-delay 90
[SwitchC-mtlk-group1] quit
# Enable L2VPN.
# Enable DCI on the Layer 3 interface that connects Switch D to Switch E for automatic VXLAN-DCI tunnel establishment.
[SwitchD] interface vlan-interface 14
[SwitchD-Vlan-interface14] dci enable
[SwitchD-Vlan-interface14] quit
[SwitchD] bgp 100
[SwitchD-bgp-default] peer 6.6.6.6 as-number 200
[SwitchD-bgp-default] peer 6.6.6.6 connect-interface loopback 0
[SwitchD-bgp-default] peer 6.6.6.6 ebgp-max-hop 64
[SwitchD-bgp-default] peer 2.2.2.2 as-number 100
[SwitchD-bgp-default] peer 2.2.2.2 connect-interface loopback 0
[SwitchD-bgp-default-evpn] peer 6.6.6.6 enable
[SwitchD-bgp-default-evpn] peer 6.6.6.6 router-mac-local
[SwitchD-bgp-default-evpn] peer 2.2.2.2 enable
[SwitchD-bgp-default-evpn] peer 2.2.2.2 next-hop-local
[SwitchD-vpn-instance-vpn1] route-distinguisher 1:2
[SwitchD-Vsi-interface2] mac-address 1-2-3
[SwitchD] evpn edge group 1.2.3.4
[SwitchD] interface loopback 2
[SwitchD-LoopBack2] ip address 1.2.3.4 32
[SwitchD-LoopBack2] quit
[SwitchD] ospf
[SwitchD-ospf-1] area 0
[SwitchD-ospf-1-area-0.0.0.0] network 1.2.3.4 0.0.0.0
[SwitchD-ospf-1] quit
[SwitchD] undo monitor-link disable
[SwitchD] monitor-link group 1
[SwitchD-mtlk-group1] port gigabitethernet 1/0/1 uplink
[SwitchD-mtlk-group1] port loopback 0 downlink
[SwitchD-mtlk-group1] downlink up-delay 90
[SwitchD-mtlk-group1] quit
6.     Configure Switch F:
# Enable L2VPN.
<SwitchF> system-view
[SwitchF] l2vpn enable
[SwitchF] vxlan tunnel mac-learning disable
[SwitchF] vxlan tunnel arp-learning disable
# Enable DCI on the Layer 3 interface that connects Switch F to Switch E for automatic VXLAN-DCI tunnel establishment.
[SwitchF] interface vlan-interface 15
[SwitchF-Vlan-interface15] dci enable
[SwitchF-Vlan-interface15] quit
# Configure BGP to advertise BGP EVPN routes. Enable nexthop replacement for routes advertised to Switch G, and enable router MAC replacement for routes advertised to and received from Switch C and Switch D.
[SwitchF] bgp 200
[SwitchF-bgp-default] peer 3.3.3.3 as-number 100
[SwitchF-bgp-default] peer 3.3.3.3 connect-interface loopback 0
[SwitchF-bgp-default] peer 3.3.3.3 ebgp-max-hop 64
[SwitchF-bgp-default] peer 4.4.4.4 as-number 100
[SwitchF-bgp-default] peer 4.4.4.4 connect-interface loopback 0
[SwitchF-bgp-default] peer 4.4.4.4 ebgp-max-hop 64
[SwitchF-bgp-default] peer 7.7.7.7 as-number 200
[SwitchF-bgp-default] peer 7.7.7.7 connect-interface loopback 0
[SwitchF-bgp-default] address-family l2vpn evpn
[SwitchF-bgp-default-evpn] peer 3.3.3.3 enable
[SwitchF-bgp-default-evpn] peer 3.3.3.3 router-mac-local
[SwitchF-bgp-default-evpn] peer 4.4.4.4 enable
[SwitchF-bgp-default-evpn] peer 4.4.4.4 router-mac-local
[SwitchF-bgp-default-evpn] peer 7.7.7.7 enable
[SwitchF-bgp-default-evpn] peer 7.7.7.7 next-hop-local
[SwitchF-bgp-default-evpn] quit
[SwitchF-bgp-default] quit
[SwitchF] ip vpn-instance vpn1
[SwitchF-vpn-instance-vpn1] route-distinguisher 1:4
[SwitchF-vpn-instance-vpn1] address-family ipv4
[SwitchF-vpn-ipv4-vpn1] vpn-target 2:2
[SwitchF-vpn-ipv4-vpn1] quit
[SwitchF-vpn-instance-vpn1] address-family evpn
[SwitchF-vpn-evpn-vpn1] vpn-target 1:1
[SwitchF-vpn-evpn-vpn1] quit
[SwitchF-vpn-instance-vpn1] quit
[SwitchF] interface vsi-interface 2
[SwitchF-Vsi-interface2] ip binding vpn-instance vpn1
[SwitchF-Vsi-interface2] l3-vni 1000
[SwitchF-Vsi-interface2] quit
7.     Configure Switch G:
# Enable L2VPN.
<SwitchG> system-view
[SwitchG] l2vpn enable
[SwitchG] vxlan tunnel mac-learning disable
[SwitchG] vxlan tunnel arp-learning disable
[SwitchG] vsi vpnb
[SwitchG-vsi-vpnb] vxlan 20
[SwitchG-vsi-vpnb-vxlan-20] quit
[SwitchG-vsi-vpnb] evpn encapsulation vxlan
[SwitchG-vsi-vpnb-evpn-vxlan] route-distinguisher auto
[SwitchG-vsi-vpnb-evpn-vxlan] vpn-target auto
[SwitchG-vsi-vpnb-evpn-vxlan] quit
[SwitchG-vsi-vpnb] quit
[SwitchG] bgp 200
[SwitchG-bgp-default] peer 6.6.6.6 as-number 200
[SwitchG-bgp-default] peer 6.6.6.6 connect-interface loopback 0
[SwitchG-bgp-default] address-family l2vpn evpn
[SwitchG-bgp-default-evpn] peer 6.6.6.6 enable
[SwitchG-bgp-default-evpn] quit
[SwitchG-bgp-default] quit
# On GigabitEthernet 1/0/1, create Ethernet service instance 2000 to match VLAN 200.
[SwitchG] interface gigabitethernet 1/0/1
[SwitchG-GigabitEthernet1/0/1] service-instance 2000
[SwitchG-GigabitEthernet1/0/1-srv2000] encapsulation s-vid 200
# Map Ethernet service instance 2000 to VSI vpnb.
[SwitchG-GigabitEthernet1/0/1-srv2000] xconnect vsi vpnb
[SwitchG-GigabitEthernet1/0/1-srv2000] quit
[SwitchG] ip vpn-instance vpn1
[SwitchG-vpn-instance-vpn1] route-distinguisher 1:4
[SwitchG-vpn-instance-vpn1] address-family ipv4
[SwitchG-vpn-ipv4-vpn1] vpn-target 2:2
[SwitchG-vpn-ipv4-vpn1] quit
[SwitchG-vpn-instance-vpn1] address-family evpn
[SwitchG-vpn-evpn-vpn1] vpn-target 1:1
[SwitchG-vpn-evpn-vpn1] quit
[SwitchG-vpn-instance-vpn1] quit
[SwitchG] interface vsi-interface 1
[SwitchG-Vsi-interface1] ip binding vpn-instance vpn1
[SwitchG-Vsi-interface1] ip address 100.1.2.1 255.255.255.0
[SwitchG-Vsi-interface1] mac-address 2-2-2
[SwitchG-Vsi-interface1] distributed-gateway local
[SwitchG-Vsi-interface1] quit
[SwitchG] interface vsi-interface 2
[SwitchG-Vsi-interface2] ip binding vpn-instance vpn1
[SwitchG-Vsi-interface2] l3-vni 1000
[SwitchG-Vsi-interface2] quit
[SwitchG] vsi vpnb
[SwitchG-vsi-vpnb] gateway vsi-interface 1
1.     Verify the configuration on EDs. (This example uses Switch C.)
# Verify that the ED has discovered Switch A and Switch F through MAC/IP advertisement routes and IP prefix advertisement routes, and has established VXLAN and VXLAN-DCI tunnels to the switches.
[SwitchC] display evpn auto-discovery macip-prefix
[SwitchC] display interface tunnel
Tunnel0
Current state: UP
Bandwidth: 64 kbps
Tunnel1
Current state: UP
Bandwidth: 64 kbps
[SwitchC] display arp vpn-instance vpn1
                               0_2
                               0_2
[SwitchC] display ip routing-table vpn-instance vpn1
2.     Verify the configuration on Switch A:
# Verify that the switch has discovered the virtual ED through MAC/IP advertisement routes and IP prefix advertisement routes, and has established a VXLAN tunnel to the virtual ED.
[SwitchA] display evpn auto-discovery macip-prefix
# Verify that the VXLAN tunnel on the switch is up.
[SwitchA] display interface tunnel
Tunnel0
Current state: UP
Bandwidth: 64 kbps
# Verify that the switch has ARP entries and routes for the VMs.
[SwitchA] display arp vpn-instance vpn1
                               0_2
[SwitchA] display ip routing-table vpn-instance vpn1
Verify that VM 1 and VM 2 can communicate when both Switch C and Switch D are working correctly and when Switch C or Switch D fails. (Details not shown.)
  • Become a Partner
  • Partner Resources
