Configuring MACsec
About MACsec
Media Access Control Security (MACsec) secures data communication on IEEE 802 LANs. MACsec provides services such as data encryption, frame integrity check, and data origin validation for frames on the MAC sublayer of the Data Link Layer. MACsec usually cooperates with 802.1X authentication to use the keys generated from MACsec Key Agreement (MKA) negotiation for authenticated users' data encryption and integerity check. This collaboration can prevent ports from processing packets from unauthenticated users or tampered packets.
Basic concepts
CA
Connectivity association (CA) is a group of participants that use the same key and key algorithm. The encryption key used by the CA participants is called a connectivity association key (CAK). The following types of CAKs are available:
·     Pairwise CAK—Used by CAs that have two participants.
·     Group CAK—Used by CAs that have more than two participants.
The pairwise CAK is used most often because MACsec is typically applied to point-to-point networks.
A CAK can be an encryption key generated during 802.1X authentication or a user-configured preshared key. The user-configured preshared key takes precedence over the 802.1X-generated key.
SA
Secure association (SA) is an agreement negotiated by CA participants. The agreement includes a cipher suite and keys for integrity check.
A secure channel can contain more than one SA. Each SA uses a unique secure association key (SAK). The SAK is generated from the CAK, and MACsec uses the SAK to encrypt data transmitted along the secure channel.
MACsec Key Agreement (MKA) limits the number of packets that can be encrypted by an SAK. When the limit is exceeded, the SAK will be refreshed. For example, when packets with the minimum size are sent on a 10-Gbps link, an SAK rekey occurs about every 300 seconds.
MACsec services
Data encryption
MACsec enables a port to encrypt outbound frames and decrypt MACsec-encrypted inbound frames. The keys for encryption and decryption are negotiated by MKA.
Integrity check
MACsec performs integrity check when the device receives a MACsec-encrypted frame. The integrity check uses the following process:
·     Uses a key negotiated by MKA to calculate an integrity check value (ICV) for the frame.
·     Compares the calculated ICV with the ICV in the frame trailer.
¡     If the ICVs are the same, the device verifies the frame as legal.
¡     If the ICVs are different, the device determines whether to drop the frame based on the validation mode. The device supports the following validation modes:
-     check—Performs validation only, and does not drop illegal frames.
-     disabled—Does not perform validation.
-     strict—Performs validation, and drops illegal frames.
Replay protection
When MACsec frames are transmitted over the network, frame disorder might occur. MACsec replay protection allows the device to accept the out-of-order packets within the replay protection window size and drop other out-of-order packets.
MACsec application modes
MACsec supports client-oriented and device-oriented modes.
Client-oriented mode
As shown in Figure 1, MACsec secures data transmission between the client and the access device. In this mode, MACsec must operate with 802.1X authentication.
Client-oriented MACsec includes the following entities:
·     Client (supplicant)—A user terminal seeking access to the LAN. The terminal must have 802.1X software to authenticate to the access device. The terminal also performs CAK negotiation and packet encryption.
·     Access device (authenticator)—Authenticates the client to control access to the LAN and performs CAK negotiation and packet encryption.
·     Authentication server—Provides AAA services for the access device. The authentication server is typically a RADIUS server. After the client passes authentication, the authentication server generates and distributes the CAK to the client and the access device.
Figure 1 Client-oriented mode
In client-oriented mode, an MKA-enabled port on the access device must perform port-based 802.1X access control. The authentication method must be EAP relay.
Device-oriented mode
As shown in Figure 2, MACsec secures data transmission between devices. In this mode, the devices do not perform identity authentication, and the same preshared key must be configured on the MACsec ports that connect the devices. The devices use the configured preshared key as the CAK.
Figure 2 Device-oriented mode
MACsec operating mechanism
Operating mechanism for client-oriented mode
Figure 3 illustrates how MACsec operates in client-oriented mode.
Figure 3 MACsec interactive process in client-oriented mode
The following shows the MACsec process:
1.     After the client passes 802.1X authentication, the RADIUS server distributes the generated CAK to the client and the access device.
2.     After receiving the CAK, the client and the access device exchange EAPOL-MKA packets.
The client and the access device exchange the MACsec capability and required parameters for session establishment. The parameters include MKA key server priority and MACsec desire.
During the negotiation process, the access device automatically becomes the key server. The key server generates an SAK from the CAK for packet encryption, and it distributes the SAK to the client.
3.     The client and the access device use the SAK to encrypt packets, and they send and receive the encrypted packets in secure channels.
4.     When the access device receives a logoff request from the client, it immediately removes the associated secure session from the port. The remove operation prevents an unauthorized client from using the secure session established by the previous authorized client to access the network.
The MKA protocol also defines a session keepalive timer. If one participant does not receive any MKA packets from the peer after the timer expires, the participant removes the established secure session. The keepalive time is 6 seconds.
Operating mechanism for device-oriented mode
As shown in Figure 4, the devices use the configured preshared keys to start the session negotiation.
Figure 4 MACsec interactive process in device-oriented mode
1.     The devices use the configured preshared keys as CAKs to exchange EAPOL-MKA packets.
They exchange the MACsec capability and required parameters for session establishment. The parameters include MKA key server priority and MACsec desire.
During the negotiation process, the port with higher MKA key server priority becomes the key server. The key server generates and distributes an SAK.
2.     The devices each use the SAK to encrypt packets and send and receive the encrypted packets in secure channels.
3.     When a device receives a logoff request from the peer, it immediately deletes the associated secure session.
If one participant does not receive any MKA packets from the peer after the session keepalive timer expires, the participant removes the established secure session. The keepalive time is 6 seconds.
Protocols and standards
IEEE 802.1X-2010, Port-Based Network Access Control
IEEE 802.1AE-2006, Media Access Control (MAC) Security
Restrictions: Hardware compatibility with MACsec
Hardware
MACsec compatibility
MSR610
No
MSR810, MSR810-W, MSR810-W-DB, MSR810-LM, MSR810-W-LM, MSR810-10-PoE, MSR810-LM-HK, MSR810-W-LM-HK, MSR810-LM-CNDE-SJK, MSR810-CNDE-SJK, MSR810-EI, MSR810-LM-EA, MSR810-LM-EI
No
MSR810-LMS, MSR810-LUS
No
MSR810-SI, MSR810-LM-SI
No
MSR810-LMS-EA, MSR810-LME
No
MSR1004S-5G, MSR1004S-5G-CN
No
MSR1104S-W, MSR1104S-W-CAT6, MSR1104S-5G-CN, MSR1104S-W-5G-CN
No
MSR2600-6-X1, MSR2600-15-X1, MSR2600-15-X1-T
No
MSR2600-10-X1
No
MSR2630
No
MSR3600-28, MSR3600-51
No
MSR3600-28-SI, MSR3600-51-SI
No
No
MSR3600-28-G-DP, MSR3600-51-G-DP
No
MSR3610-I-DP, MSR3610-IE-DP, MSR3610-IE-ES, MSR3610-IE-EAD, MSR-EAD-AK770, MSR3610-I-IG, MSR3610-IE-IG
No
MSR3610-X1, MSR3610-X1-DP, MSR3610-X1-DC, MSR3610-X1-DP-DC, MSR3620-X1, MSR3640-X1
No
MSR3610, MSR3620, MSR3620-DP, MSR3640, MSR3660
No
MSR3610-G, MSR3620-G
No
MSR3640-G
No
MSR3640-X1-HI
Yes
Hardware
MSR810-W-WiNet, MSR810-LM-WiNet
No
MSR830-4LM-WiNet
No
MSR830-5BEI-WiNet, MSR830-6EI-WiNet, MSR830-10BEI-WiNet
No
MSR830-6BHI-WiNet, MSR830-10BHI-WiNet
No
MSR2600-6-WiNet
No
MSR2600-10-X1-WiNet
No
MSR2630-WiNet
No
MSR3600-28-WiNet
No
MSR3610-X1-WiNet
No
MSR3610-WiNet, MSR3620-10-WiNet, MSR3620-DP-WiNet, MSR3620-WiNet, MSR3660-WiNet
No
Hardware
MSR860-6EI-XS
No
MSR860-6HI-XS
No
MSR2630-XS
No
MSR3600-28-XS
No
MSR3610-XS
No
MSR3620-XS
No
MSR3610-I-XS
No
MSR3610-IE-XS
No
MSR3620-X1-XS
No
MSR3640-XS
No
MSR3660-XS
Yes
Hardware
MSR810-LM-GL
No
MSR810-W-LM-GL
No
MSR830-6EI-GL
No
MSR830-10EI-GL
No
MSR830-6HI-GL
No
MSR830-10HI-GL
No
MSR1004S-5G-GL
No
MSR2600-6-X1-GL
No
MSR3600-28-SI-GL
No
MACsec tasks at a glance
To configure MACsec, perform the following tasks:
1.     Enabling MKA
2.     Enabling MACsec desire
3.     Specifying the cipher suite for MACsec encryption
4.     Configuring a preshared key
This task is required in device-oriented mode. Do not perform this task in client-oriented mode.
5.     (Optional.) Configuring the MKA key server priority
6.     (Optional.) Setting the MKA life time
7.     (Optional.) Configuring MACsec protection parameters
¡     Configuring MACsec protection parameters in interface view
¡     Configuring MACsec protection parameters by MKA policy
8.     (Optional.) Enabling MKA session logging
Enabling MKA
MKA establishes and manages MACsec secure channels on a port. It also negotiates keys used by MACsec.
2.     Enter interface view.
3.     Enable MKA.
mka enable
By default, MKA is disabled on the port.
The MACsec desire feature expects MACsec protection for outbound frames. The key server determines whether MACsec protects the outbound frames.
MACsec protects the outbound frames of a port when the following requirements are met:
·     The key server is MACsec capable.
·     Both the local participant and its peer are MACsec capable.
·     A minimum of one participant is enabled with MACsec desire.
3.     Enable MACsec desire.
macsec desire
By default, the port does not expect MACsec protection for outbound frames.
MACsec uses the GCM-AES-128 or GCM-AES-256 cipher suite to encrypt, validate, and decrypt protected data frames.
This feature is supported only in device-oriented mode. Do not configure this feature on an 802.1X-enabled port.
Make sure the connected MACsec ports are configured with the same cipher suite. If the ports are configured with different cipher suites, they cannot successfully establish MKA sessions.
3.     Specify the cipher suite for MACsec encryption.
macsec cipher-suite { gcm-aes-128 | gcm-aes-256 }
By default, MACsec uses the GCM-AES-128 cipher suite for encryption.
In device-oriented mode, configure a preshared key as the CAK to be used during MKA negotiation. To successfully establish an MKA session between two devices, make sure the following requirements are met:
·     The connected MACsec ports are configured with the same CAK and CKN.
·     Only the ports are configured with the same CKN in the network.
A user-configured preshared key has higher priority than the 802.1X-generated CAK. To ensure a successful MKA session establishment, do not configure a preshared key in client-oriented mode.
Different cipher suites for MACsec encryption have different requirements for the CKN and CAK configuration.
·     The GCM-AES-128 cipher suite requires that the CKN and CAK each must be 32 characters long. If the configured CKN or CAK is not 32 characters long, the system performs the following operations when it runs the cipher suite:
¡     Automatically increases the length of the CKN or CAK by zero padding if the CKN or CAK contains less than 32 characters.
¡     Uses only the first 32 characters if the CKN or CAK contains more than 32 characters.
·     The GCM-AES-256 cipher suite requires that the CKN and CAK each must be 64 characters long. If the configured CKN or CAK contains less than 64 characters, the system automatically increases the length of the CKN or CAK by zero padding when it runs the cipher suite.
3.     Set a preshared key.
mka psk ckn name cak { cipher | simple } string
By default, no MKA preshared key exists.
The MACsec cipher suite supported by the device requires that the CKN and CAK each must be 32 characters long. If the configured CKN or CAK is not 32 characters long, the system performs the following operations when it runs the cipher suite:
When you configure the MKA key server priority, follow these restrictions and guidelines:
·     In client-oriented mode, the access device port automatically becomes the key server. You do not have to configure the MKA key server priority.
·     In device-oriented mode, the port that has higher priority becomes the key server. The lower the priority value, the higher the priority. If a port and its peers have the same priority, MACsec compares the secure channel identifier (SCI) values on the ports. The port with the lowest SCI value (a combination of MAC address and port ID) becomes the key server.
·     A port with priority 255 cannot become the key server. For a successful key server selection, make sure a minimum of one participant's key server priority is not 255.
3.     Set the MKA key server priority.
mka priority priority-value
The default setting is 0.
This task is applicable only in device-oriented mode.
Make sure the participants at each end of a secure session have the same MKA life time.
3.     Set the MKA life time.
mka timer mka-life seconds
By default, the MKA life time is 6 seconds.
About MACsec protection parameters
You can set the following MACsec protection parameters:
·     MACsec confidentiality offset—Specifies the number of bytes starting from the frame header. MACsec encrypts only the bytes after the offset in a frame. The offset value can be 0, 30, or 50.
·     MACsec replay protection—Allows a MACsec port to accept a number of out-of-order or repeated inbound frames.
·     MACsec validation—Allows a port to perform integrity check based on the validation modes.
Restrictions and guidelines for MACsec protection parameter configuration
You can configure MACsec protection parameters either in interface view or through MKA policies.
The use of MKA policies provides a centralized method to configure MACsec protection parameters. When you need to configure the same settings for MACsec protection parameters on multiple ports, you can configure them in an MKA policy and apply the policy to the ports.
If you configure a protection parameter in interface view after applying an MKA policy, the configuration in interface view overwrites the configuration of that parameter in the MKA policy. The other protection parameters in the MKA policy still take effect.
If you apply an MKA policy to a port after configuring protection parameters on the port, the settings in the policy overwrite all protection parameter settings in interface view. The protection parameters not configured in the policy are restored to the default.
3.     Set the MACsec confidentiality offset.
macsec confidentiality-offset offset-value
The default setting is 0, and the entire frame needs to be encrypted.
MACsec uses the confidentiality offset propagated by the key server.
4.     Configure MACsec replay protection:
a.     Enable MACsec replay protection.
macsec replay-protection enable
By default, MACsec replay protection is enabled on the port.
b.     Set the MACsec replay protection window size.
macsec replay-protection window-size size-value
The default setting is 0. The device accepts only frames that arrive in the correct order. Out-of-order or duplicated frames will be dropped.
The configured replay protection window size takes effect only when MACsec replay protection is enabled.
5.     Set a MACsec validation mode.
macsec validation mode { check | disabled| strict }
The default setting is check.
To avoid data loss, use the display macsec command to verify that MKA negotiation with the peer device has succeeded before you change the mode to strict.
Parameter
check
Verifies incoming frames but does not drop illegal frames.
disabled
Disables MACsec validation for incoming frames.
strict
Verifies incoming frames and drops illegal frames.
An MKA policy can be applied to a port or multiple ports. When you apply an MKA policy to a port, follow these restrictions and guidelines:
·     The settings in the MKA policy overwrite all protection parameter settings configured in interface view. The protection parameters not configured in the policy are restored to the default.
·     Any modifications to the MKA policy take effect immediately.
·     When you remove an MKA policy application from the port, the MACsec parameter settings on the port restore to the default.
·     When you apply a nonexistent MKA policy to the port, the port automatically uses the system-defined MKA policy named default-policy. If you create the policy, the policy will be automatically applied to the port.
2.     Create an MKA policy and enter its view.
mka policy policy-name
By default, a system-defined MKA policy exists. The policy name is default-policy.
The settings for parameters in the system-defined policy are the same as the default settings for the parameters on a port.
You cannot delete or modify the system-defined MKA policy.
You can create multiple MKA policies.
By default, MACsec replay protection is enabled.
b.     Set the replay protection window size.
The default replay protection window size is 0. The device accepts only frames that arrive in the correct order. Out-of-order or duplicated frames will be dropped.
validation mode { check | disabled | strict }
Parameter
check
disabled
strict
6.     Apply an MKA policy:
a.     Return to system view.
b.     Enter interface view.
c.     Apply the MKA policy to the port.
mka apply policy policy-name
By default, no MKA policy is applied to a port.
This feature enables the device to generate logs for MKA session changes, such as peer aging and SAK updates. The logs are sent to the information center of the device. For the logs to be output correctly, you must also configure the information center on the device. For more information about information center configuration, see Network Management and Monitoring Configuration Guide.
As a best practice, disable this feature to prevent excessive MKA session log output.
2.     Enable MKA session logging.
macsec mka-session log enable
By default, MKA session logging is disabled.
Display and maintenance commands for MACsec
Display MACsec information on ports.
display macsec [ interface interface-type interface-number ] [ verbose ]
Display MKA policy information.
display mka { default-policy | policy [ name policy-name ] }
Display MKA session information.
display mka session [ interface interface-type interface-number | local-sci sci-id ] [ verbose ]
Display MKA statistics on ports.
display mka statistics [ interface interface-type interface-number ]
Reset MKA sessions on ports.
reset mka session [ interface interface-type interface-number ]
Clear MKA statistics on ports.
reset mka statistics [ interface interface-type interface-number ]
MACsec configuration examples
Example: Configuring client-oriented MACsec
As shown in Figure 5, the host accesses the network through GigabitEthernet 1/0/1. The device performs RADIUS-based 802.1X authentication for the host to control user access to the Internet.
To ensure secure communication between the host and device, perform the following tasks on the device:
·     Enable MACsec desire, and configure MKA to negotiate SAKs for packet encryption.
·     Set the MACsec confidentiality offset to 30 bytes.
·     Enable MACsec replay protection, and set the replay protection window size to 100.
·     Set the MACsec validation mode to strict.
Figure 5 Network diagram
1.     Configure IP addresses for the Ethernet ports. (Details not shown.)
2.     Configure the RADIUS server to provide authentication, authorization, and accounting services. Add a user account for the host. (Details not shown.)
3.     Configure AAA:
# Enter system view.
# Configure RADIUS scheme radius1.
[Device] radius scheme radius1
[Device-radius-radius1] primary authentication 10.1.1.1
[Device-radius-radius1] primary accounting 10.1.1.1
[Device-radius-radius1] key authentication simple name
[Device-radius-radius1] key accounting simple name
[Device-radius-radius1] user-name-format without-domain
[Device-radius-radius1] quit
# Configure authentication domain bbb for 802.1X users.
[Device] domain bbb
[Device-isp-bbb] authentication lan-access radius-scheme radius1
[Device-isp-bbb] authorization lan-access radius-scheme radius1
[Device-isp-bbb] accounting lan-access radius-scheme radius1
[Device-isp-bbb] quit
4.     Configure 802.1X:
# Enable 802.1X on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] dot1x
# Implement port-based access control on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] dot1x port-method portbased
# Specify bbb as the mandatory authentication domain for 802.1X users on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] dot1x mandatory-domain bbb
# Enable 802.1X globally, and sets the device to relay EAP packets.
[Device] dot1x
[Device] dot1x authentication-method eap
5.     Configure MACsec:
# Create an MKA policy named pls.
[Device] mka policy pls
# Set the MACsec confidentiality offset to 30 bytes.
[Device-mka-policy-pls] confidentiality-offset 30
# Enable MACsec replay protection.
[Device-mka-policy-pls] replay-protection enable
# Set the MACsec replay protection window size to 100.
[Device-mka-policy-pls] replay-protection window-size 100
# Set the MACsec validation mode to strict.
[Device-mka-policy-pls] validation mode strict
[Device-mka-policy-pls] quit
# Apply the MKA policy to GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] mka apply policy pls
# Configure MACsec desire and enable MKA on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] macsec desire
[Device-GigabitEthernet1/0/1] mka enable
# Display MACsec information on GigabitEthernet 1/0/1.
[Device] display macsec interface gigabitethernet 1/0/1 verbose
  Protect frames         : Yes
  Active MKA policy      : pls
  Replay protection      : Enabled
  Replay window size     : 100 frames
  Confidentiality offset : 30 bytes
  Validation mode        : Strict
  Included SCI           : No
  SCI conflict           : No
  Cipher suite           : GCM-AES-128
  Transmit secure channel:
    SCI           : 00E00100000A0006
      Elapsed time: 00h:02m:07s
      Current SA  : AN 0        PN 1
  Receive secure channels:
    SCI           : 00E0020000000106
      Elapsed time: 00h:02m:03s
      Current SA  : AN 0        LPN 1
      Previous SA : AN N/A      LPN N/A
# Display MKA session information on GigabitEthernet 1/0/1 after a user logs in.
[Device] display mka session interface gigabitethernet 1/0/1 verbose
Tx-SCI    : 00E00100000A0006
Priority  : 0
Capability: 3
  CKN for participant: 1234
    Key server            : Yes
    MI (MN)               : A1E0D2897596817209CD2307 (2509)
    Live peers            : 1
    Potential peers       : 0
    Principal actor       : Yes
    MKA session status    : Secured
    Confidentiality offset: 30 bytes
    Current SAK status    : Rx & Tx
    Current SAK AN        : 0
    Current SAK KI (KN)   : A1E0D2897596817209CD230700000002 (2)
    Previous SAK status   : N/A
    Previous SAK AN       : N/A
    Previous SAK KI (KN)  : N/A
    Live peer list:
    MI                        MN         Priority  Capability  Rx-SCI
    B2CAF896C9BFE2ABFB135E63  2512       0         3           00E0020000000106
Example: Configuring device-oriented MACsec
As shown in Figure 6, Device A is the MACsec key server.
To secure data transmission between the two devices by MACsec, perform the following tasks on Device A and Device B, respectively:
·     Configure the CAK name (CKN) and the CAK as E9AC and 09DB3EF1, respectively.
Figure 6 Network diagram
1.     Configure Device A:
# Enter GigabitEthernet 1/0/1 interface view.
# Enable MACsec desire on GigabitEthernet 1/0/1.
[DeviceA-GigabitEthernet1/0/1] macsec desire
# Set the MKA key server priority to 5.
[DeviceA-GigabitEthernet1/0/1] mka priority 5
# Configure the CKN as E9AC and the CAK as 09DB3EF1 in plain text.
[DeviceA-GigabitEthernet1/0/1] mka psk ckn E9AC cak simple 09DB3EF1
[DeviceA-GigabitEthernet1/0/1] macsec confidentiality-offset 30
[DeviceA-GigabitEthernet1/0/1] macsec replay-protection enable
[DeviceA-GigabitEthernet1/0/1] macsec replay-protection window-size 100
[DeviceA-GigabitEthernet1/0/1] macsec validation mode strict
# Enable MKA on GigabitEthernet 1/0/1.
[DeviceA-GigabitEthernet1/0/1] mka enable
2.     Configure Device B:
[DeviceB-GigabitEthernet1/0/1] macsec desire
# Set the MKA key server priority to 10.
[DeviceB-GigabitEthernet1/0/1] mka priority 10
[DeviceB-GigabitEthernet1/0/1] mka psk ckn E9AC cak simple 09DB3EF1
[DeviceB-GigabitEthernet1/0/1] macsec confidentiality-offset 30
[DeviceB-GigabitEthernet1/0/1] macsec replay-protection enable
[DeviceB-GigabitEthernet1/0/1] macsec replay-protection window-size 100
[DeviceB-GigabitEthernet1/0/1] macsec validation mode strict
[DeviceB-GigabitEthernet1/0/1] mka enable
# Display MACsec information on GigabitEthernet 1/0/1 of Device A.
[DeviceA] display macsec interface gigabitethernet 1/0/1 verbose
  Included SCI           : No
  SCI conflict           : No
      Elapsed time: 00h:05m:00s
      Elapsed time: 00h:03m:18s
# Display MKA session information on GigabitEthernet 1/0/1 of Device A.
[DeviceA] display mka session interface gigabitethernet 1/0/1 verbose
Priority  : 5
Capability: 3
  CKN for participant: E9AC
    Key server            : Yes
    MI (MN)               : 85E004AF49934720AC5131D3 (182)
    Live peers            : 1
    Potential peers       : 0
    Current SAK AN        : 0
    Current SAK KI (KN)   : 85E004AF49934720AC5131D300000003 (3)
    Live peer list:
    12A1677D59DD211AE86A0128  182        10        3           00E0020000000106
# Display MACsec information on GigabitEthernet 1/0/1 of Device B.
[DeviceB] display macsec interface gigabitethernet 1/0/1 verbose
  Included SCI           : No
  SCI conflict           : No
      Elapsed time: 00h:05m:36s
      Elapsed time: 00h:03m:21s
# Display MKA session information on GigabitEthernet 1/0/1 of Device B.
[DeviceB] display mka session interface gigabitethernet 1/0/1 verbose
Tx-SCI    : 00E0020000000106
Priority  : 10
Capability: 3
    Key server            : No
    MI (MN)               : 12A1677D59DD211AE86A0128 (1219)
    Live peers            : 1
    Potential peers       : 0
    Current SAK AN        : 0
    Live peer list:
    85E004AF49934720AC5131D3  1216       5         3           00E00100000A0006
Troubleshooting MACsec
Cannot establish MKA sessions between MACsec devices
Symptom
The devices cannot establish MKA sessions when the following conditions exist:
·     The link connecting the devices is up.
·     The ports at the ends of the link are MACsec capable.
Analysis
The symptom might occur for the following reasons:
·     The ports at the link are not enabled with MKA.
·     A port at the link is not configured with a preshared key or configured with a preshared key different from the peer.
Solution
To resolve the issue:
1.     Enter interface view.
2.     Use the display this command to check the MACsec configuration:
¡     If MKA is not enabled on the port, execute the mka enable command.
¡     If a preshared key is not configured or the preshared key is different from the peer, use the mka psk command to configure a preshared key. Make sure the preshared key is the same as the preshared key on the peer.
3.     If the issue persists, contact H3C Support.
  • Become a Partner
  • Partner Resources