- 01-AAA configuration
- 02-802.1X configuration
- 04-Portal configuration
- 05-Web authentication configuration
- 06-Triple authentication configuration
- 07-Port security configuration
- 08-Password control configuration
- 09-Keychain configuration
- 10-Public key management
- 11-PKI configuration
- 12-IPsec configuration
- 13-SSH configuration
- 14-SSL configuration
- 15-Attack detection and prevention configuration
- 16-TCP attack prevention configuration
- 17-IP source guard configuration
- 18-ARP attack protection configuration
- 19-ND attack defense configuration
- 20-uRPF configuration
- 21-MFF configuration
- 22-FIPS configuration
- 23-MACsec configuration
- 24-802.1X client configuration
| 19-ND attack defense configuration | 139.85 KB |
ND attack defense tasks at a glance
Enabling source MAC consistency check for ND messages
Configuring ND attack detection
Restrictions and guidelines for ND attack detection configuration
Configuring ND attack detection for a VLAN
Ignoring ingress ports of ND packets
Enabling ND attack detection logging
Display and maintenance commands for ND attack detection
Example: Configuring ND attack detection
Specifying the role of the attached device
Configuring and applying an RA guard policy
Enabling the RA guard logging feature
Display and maintenance commands for RA guard
Configuring ND keepalive entry scanning
About ND keepalive entry scanning
Display and maintenance commands for ND keepalive entry scanning
Enabling SNMP notifications for ND
Configuring ND attack defense
About ND attack defense
IPv6 Neighbor Discovery (ND) attack defense is able to identify forged ND messages to prevent ND attacks.
The IPv6 ND protocol does not provide any security mechanisms and is vulnerable to network attacks. As shown in Figure 1, an attacker can send the following forged ICMPv6 messages to perform ND attacks:
· Forged NS/NA/RS messages with an IPv6 address of a victim host. The gateway and other hosts update the ND entry for the victim with incorrect address information. As a result, all packets intended for the victim are sent to the attacking terminal.
· Forged RA messages with the IPv6 address of a victim gateway. As a result, all hosts attached to the victim gateway maintain incorrect IPv6 configuration parameters and ND entries.
All ND attack defense tasks are optional.
· Enabling source MAC consistency check for ND messages
· Configuring ND attack detection
· Configuring ND keepalive entry scanning
· Enabling SNMP notifications for ND
The source MAC consistency check feature is typically configured on gateways to prevent ND attacks.
This feature checks the source MAC address and the source link-layer address for consistency for each arriving ND message.
· If the source MAC address and the source link-layer address are not the same, the device drops the packet.
· If the addresses are the same, the device continues learning ND entries.
The ND logging feature logs source MAC inconsistency events, and it sends the log messages to the information center. The information center can then output log messages from different source modules to different destinations. For more information about the information center, see Network Management and Monitoring Configuration Guide.
1. Enter system view.
2. Enable source MAC consistency check for ND messages.
ipv6 nd mac-check enable
By default, source MAC consistency check is disabled for ND messages.
3. (Optional.) Enable the ND logging feature.
ipv6 nd check log enable
By default, the ND logging feature is disabled.
As a best practice, disable the ND logging feature to avoid excessive ND logs.
About ND attack detection
ND attack detection checks incoming ND messages for user validity to prevent spoofing attacks. It is typically configured on access devices.
ND attack detection defines the following types of interfaces on a VLAN network:
· ND trusted interface—Performs no user validity check on the received ND messages.
· ND untrusted interface—Discards incoming RA and redirect messages, and performs the user validity check on other types of incoming ND messages.
ND attack detection compares the source IPv6 address and the source MAC address in an incoming ND message against security entries from other modules.
· If a match is found, the device verifies the user as legal, and it forwards the packet.
· If no match is found, the device verifies the user as illegal, and it discards the ND message.
ND attack detection uses static IPv6 source guard binding entries, ND snooping entries, and DHCPv6 snooping entries for user validity check.
· Static IPv6 source guard binding entries are created by using the ipv6 source binding command. For information about IPv6 source guard, see "Configuring IP source guard."
· ND snooping entries are automatically generated by the ND snooping feature. For information about ND snooping, see IPv6 neighbor discovery configuration in Layer 3–IP Services Configuration Guide.
· DHCPv6 snooping entries are automatically generated by the DHCPv6 snooping feature. For information about DHCPv6 snooping, see Layer 3–IP Services Configuration Guide.
When you configure ND attack detection, follow these restrictions and guidelines:
· To prevent ND untrusted interfaces from dropping all received ND messages, make sure one or more of the these features are configured: IPv6 source guard static bindings, DHCPv6 snooping, and ND snooping.
· To make the IPv6 source guard static bindings effective for ND attack detection, you must perform the following operations:
¡ Specify the vlan vlan-id option in the ipv6 source binding command.
¡ Enable ND attack detection for the same VLAN.
2. Enter VLAN view.
vlan vlan-id
3. Enable ND attack detection.
ipv6 nd detection enable
By default, ND attack detection is disabled.
4. (Optional.) Configure the interface as ND trusted interface:
a. Return to system view.
b. Enter Layer 2 Ethernet or aggregate interface view.
c. Configure the interface as ND trusted interface.
ipv6 nd detection trust
By default, all interfaces are ND untrusted interfaces.
With ND attack detection enabled, the device can perform security check on received packets based on the local and remote IPSG bindings. Remote IPSG bindings do not contain port information. The device drops ND packets that match remote IPSG bindings because it does not find matching ingress ports for these packets. To prevent the device from dropping these packets, you can configure the device to ignore ingress ports of ND packets. This feature does not examine the ingress ports of ND packets, so that ND packets that match remote IPSG bindings will not be dropped.
2. Ignore ingress ports of ND packets in ND attack detection.
ipv6 nd detection port-match-ignore
By default, ingress ports of ND packets are examined in ND attack detection.
This feature allows a device to generate logs when it detects invalid ND packets. The log information helps administrators locate and solve problems. Each log records the following information:
· Victim port numbers in a VLAN.
· Source IP address of the invalid ND packets.
· Source MAC address of the invalid ND packets.
· VLAN ID of the invalid ND packets.
· Total number of dropped ND packets.
2. Enable ND attack detection logging.
ipv6 nd detection log enable
By default, ND attack detection logging is disabled.
Task |
Command |
Display statistics for ND messages dropped by ND attack detection. |
display ipv6 nd detection statistics [ interface interface-type interface-number ] |
Clear ND attack detection statistics. |
reset ipv6 nd detection statistics [ interface interface-type interface-number ] |
As shown in Figure 2, configure ND attack detection on Device B to check user validity for ND messages from Host A and Host B.
# Create VLAN 10.
[DeviceA] vlan 10
[DeviceA-vlan10] quit
# Configure GigabitEthernet 1/0/3 to trunk VLAN 10.
[DeviceA-GigabitEthernet1/0/3] port link-type trunk
[DeviceA-GigabitEthernet1/0/3] port trunk permit vlan 10
# Assign IPv6 address 10::1/64 to VLAN-interface 10.
[DeviceA-Vlan-interface10] ipv6 address 10::1/64
2. Configure Device B:
# Create VLAN 10.
[DeviceB] vlan 10
[DeviceB-vlan10] quit
# Configure GigabitEthernet 1/0/1, GigabitEthernet 1/0/2, and GigabitEthernet 1/0/3 to trunk VLAN 10.
[DeviceB-GigabitEthernet1/0/1] port link-type access
[DeviceB-GigabitEthernet1/0/1] port access vlan 10
[DeviceB-GigabitEthernet1/0/2] port link-type access
[DeviceB-GigabitEthernet1/0/2] port access vlan 10
[DeviceB] interface gigabitethernet 1/0/3
[DeviceB-GigabitEthernet1/0/3] port link-type trunk
[DeviceB-GigabitEthernet1/0/3] port trunk permit vlan 10
# Enable ND attack detection for VLAN 10.
[DeviceB] vlan 10
[DeviceB-vlan10] ipv6 nd detection enable
# Enable ND snooping for IPv6 global unicast addresses and ND snooping for IPv6 link-local addresses in VLAN 10.
[DeviceB-vlan10] ipv6 nd snooping enable global
[DeviceB-vlan10] ipv6 nd snooping enable link-local
# Configure GigabitEthernet 1/0/3 as ND trusted interface.
[DeviceB-GigabitEthernet1/0/3] ipv6 nd detection trust
Verify that Device B inspects all ND messages received by GigabitEthernet 1/0/1 and GigabitEthernet 1/0/2 based on the ND snooping entries. (Details not shown.)
Configuring RA guard
About RA guard
RA guard allows Layer 2 access devices to analyze and block unwanted and forged RA messages.
Upon receiving an RA message, the device makes the forwarding or dropping decision based on the role of the attached device or the RA guard policy.
1. If the role of the device attached to the receiving interface is router, the device forwards the RA message. If the role is host, the device drops the RA message.
2. If no attached device role is set, the device uses the RA guard policy applied to the VLAN of the receiving interface to match the RA message.
¡ If the policy does not contain match criteria, the policy will not take effect and the device forwards the RA message.
¡ If the RA message content matches every criterion in the policy, the device forwards the message. Otherwise, the device drops the message.
Make sure your setting is consistent with the type of the attached device. If you are not aware of the device type, do not specify a role for the device.
2. Enter interface view.
¡ Enter aggregate interface view.
3. Specify the role of the device attached to the interface.
ipv6 nd raguard role { host | router }
By default, the role of the device attached to the interface is not specified.
Configure an RA guard policy if you do not specify a role for the attached device or if you want to filter the RA messages sent by a router.
2. Create an RA guard policy and enter its view.
ipv6 nd raguard policy policy-name
3. Configure the RA guard policy.
¡ Specify an ACL match criterion.
¡ Specify a prefix match criterion.
if-match prefix acl { ipv6-acl-number | name ipv6-acl-name }
¡ Specify a router preference match criterion.
if-match router-preference maximum { high | low | medium }
¡ Specify an M flag match criterion.
if-match autoconfig managed-address-flag { off | on }
¡ Specify an O flag match criterion.
if-match autoconfig other-flag { off | on }
¡ Specify a maximum or minimum hop limit match criterion.
if-match hop-limit { maximum | minimum } limit
By default, the RA guard policy is not configured.
4. Quit RA guard policy view.
5. Enter VLAN view.
vlan vlan-number
6. Apply an RA guard policy to the VLAN.
ipv6 nd raguard apply policy [ policy-name ]
By default, no RA guard policy is applied to the VLAN.
This feature allows a device to generate logs when it detects forged RA messages. The log information helps administrators locate and solve problems. Each log records the following information:
· Name of the interface that received the forged RA message.
· Source IP address of the forged RA message.
· Number of RA messages dropped on the interface.
The RA guard logging feature sends the log messages to the information center. The information center can then output log messages from different source modules to different destinations. For more information about the information center, see Network Management and Monitoring Configuration Guide.
2. Enable the RA guard logging feature.
ipv6 nd raguard log enable
By default, the RA guard logging feature is disabled.
Task |
Command |
Display the RA guard policy configuration. |
display ipv6 nd raguard policy [ policy-name ] |
Display RA guard statistics. |
display ipv6 nd raguard statistics [ interface interface-type interface-number ] |
Clear RA guard statistics. |
reset ipv6 nd raguard statistics [ interface interface-type interface-number ] |
Example: Configuring RA guard
As shown in Figure 3, GigabitEthernet 1/0/1, GigabitEthernet 1/0/2, and GigabitEthernet 1/0/3 of Device B are in VLAN 10.
Configure RA guard on Device B to filter forged and unwanted RA messages.
· Configure an RA policy in VLAN 10 for GigabitEthernet 1/0/2 to filter all RA messages received from the unknown device.
· Specify host as the role of the host. All RA messages received on GigabitEthernet 1/0/1 are dropped.
· Specify router as the role of the Device A. All RA messages received on GigabitEthernet 1/0/3 are forwarded.
# Create an RA guard policy named policy1.
[DeviceB] ipv6 nd raguard policy policy1
# Set the maximum router preference to high for the RA guard policy.
[DeviceB-raguard-policy-policy1] if-match router-preference maximum high
# Specify on as the M flag match criterion for the RA guard policy.
[DeviceB-raguard-policy-policy1] if-match autoconfig managed-address-flag on
# Specify on as the O flag match criterion for the RA guard policy.
[DeviceB-raguard-policy-policy1] if-match autoconfig other-flag on
# Set the maximum advertised hop limit to 120 for the RA guard policy.
[DeviceB-raguard-policy-policy1] if-match hop-limit maximum 120
# Set the minimum advertised hop limit to 100 for the RA guard policy.
[DeviceB-raguard-policy-policy1] if-match hop-limit minimum 100
[DeviceB-raguard-policy-policy1] quit
# Assign GigabitEthernet 1/0/1 and GigabitEthernet 1/0/2 to VLAN 10.
# Apply the RA guard policy policy1 to VLAN 10.
[DeviceB] vlan 10
[DeviceB-vlan10] ipv6 nd raguard apply policy policy1
# Specify host as the role of the device attached to GigabitEthernet 1/0/1.
[DeviceB-GigabitEthernet1/0/1] ipv6 nd raguard role host
# Specify router as the role of the device attached to GigabitEthernet 1/0/3.
[DeviceB-GigabitEthernet1/0/3] ipv6 nd raguard role router
# Verify that the device forwards or drops RA messages received on GigabitEthernet 1/0/2 based on the RA guard policy. (Details not shown.)
# Verify that the device drops RA messages received on GigabitEthernet 1/0/1. (Details not shown.)
# Verify that the device forwards RA messages received on GigabitEthernet 1/0/3 to other interfaces in VLAN 10. (Details not shown.)
In a large-scale network, it takes a long time for ND scanning to identify the hosts that go offline abnormally if you specify a large scanning range. After you enable ND keepalive entry scanning, the system can quickly locate those hosts and monitor the host status within the aging time.
When users come online, the system generates dynamic ND entries and IPSG binding entries. Enabled with ND keepalive entry scanning, the system also creates online keepalive entries when users come online. If users go offline, the corresponding ND entries are deleted and the status of the keepalive entries is set to offline. The device sends NS packets at intervals to the IPv6 addresses in the offline keepalive entries until the keepalive entries become online again or are deleted when the aging time expires. The interval varies with the number of NS packets that have been sent to the IPv6 address in an offline keepalive entry. For more information about IP source guard configuration, see Security Configuration Guide.
2. (Optional.) Set the NS packet sending rate for keepalive entry scanning.
ipv6 nd scan keepalive send-rate pps
By default, the device sends NS packets at a rate of 48 pps during keepalive entry scanning.
3. (Optional.) Set the aging time for ND keepalive entries.
ipv6 nd scan keepalive aging-time time
By default, the aging time for ND keepalive entries is 60 minutes.
4. Enter interface view.
5. Enable the ND keepalive entry scanning feature.
ipv6 nd scan keepalive enable
By default, the ND keepalive entry scanning is disabled on an interface.
Task |
Command |
Display ND keepalive entries. |
display ipv6 nd scan keepalive entry [ interface interface-type interface-number ] [ count ] |
Display statistics about NS packets sent to the IPv6 addresses in offline keepalive entries. |
display ipv6 nd scan keepalive statistics [ slot slot-number ] [ interface interface-type interface-number ] |
Clear statistics about NS packets sent to the IPv6 addresses in offline keepalive entries. |
reset ipv6 nd scan keepalive statistics [ slot slot-number ] |
Enable SNMP notifications for ND as required.
· If you enable ND entry limit notifications, the device sends the current ND entry information as a notification to the SNMP module when the number of ND entries exceeds the alarm threshold.
· If you enable endpoints and local device conflict notifications, the device sends a notification to the SNMP module when an endpoint and local device conflict occurs. The notification includes the source IPv6 address, source MAC address, destination IPv6 address, and destination MAC address in the conflicting ND packet.
· If you enable sending rate limit notifications for ND Miss messages and ND packets, the device sends the highest threshold-crossed rate as a notification to the SNMP module. When the device receives an IP packet in which the destination IP address is unresolvable, it sends a ND Miss message to the CPU.
For ND event notifications to be sent correctly, you must also configure SNMP on the device. For more information, see SNMP configuration in Network Management and Monitoring Configuration Guide.
2. Enable SNMP notifications for ND.
snmp-agent trap enable nd [ entry-limit | local-conflict | nd-miss | rate-limit ] *
By default, SNMP notifications for ND are disabled.
If you do not specify any keywords, this command enables all SNMP notifications for ND.