08-Layer 3 - IP Services
HomeSupportRoutersCR16000-F SeriesReference GuidesMIB CompanionH3C CR16000-F Routers MIB Reference-R838x-6W10008-Layer 3 - IP Services
08-HH3C-DHCP6-MIB
08-HH3C-DHCP6-MIB 261.30 KB
HH3C-DHCP6-MIB
About this MIB
Use this MIB to configure DHCPv6, obtain DHCPv6 address/prefix allocation information, and configure alarm settings.
MIB file name
hh3c-dhcp6.mib
Root object
iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).hh3c(25506).hh3cCommon(2).hh3cDhcp6(179)
Scalar objects
hh3cDhcp6Server2OnlineFailReason (1.3.6.1.4.1.25506.2.179.3.1.1)
Object (OID)
Access
Value range
Implementation
accessible-for-notify
OCTET STRING
Standard MIB values.
Reason for the DHCPv6 server online failure.
As per the MIB.
Tabular objects
hh3cDhcp6Server2PoolTable
About this table
The table records the DHCPv6 address pool configuration parameters.
Support for operations
CreateSupported
It must be bound to hh3cDhcp6Server2PoolName when a row is created.
Edit/ModifyNot supported.
It cannot be modified after the hh3cDhcp6Server2PoolName is created.
DeleteSupported
ReadSupported
Columns
The table index is hh3cDhcp6Server2PoolIndex.
Object (OID)
Access
Value range
Implementation
hh3cDhcp6Server2PoolIndex (1.3.6.1.4.1.25506.2.179.1.1.1.1)
Unsigned32
Implementation varies by product
DHCPv6 address pool index.
hh3cDhcp6Server2PoolName (1.3.6.1.4.1.25506.2.179.1.1.1.2)
read-create
OCTET STRING
OCTET STRING (1..63)
DHCPv6 address pool name.
As per the MIB.
hh3cDhcp6Server2PoolRowStatus
(1.3.6.1.4.1.25506.2.179.1.1.1.3)
read-create
RowStatus
Active(1)
createAndGo(4)
destroy(6)
Row status.
As per the MIB.
hh3cDhcp6Server2PoolVpnName (1.3.6.1.4.1.25506.2.179.1.1.1.4)
read-create
OCTET STRING
OCTET STRING (0..31)
VPN instance bound to the IPv6 address pool.
You can bind a VPN instance to an IPv6 address pool only when you create the pool and cannot change the binding after pool creation.
hh3cDhcp6Server2PoolType (1.3.6.1.4.1.25506.2.179.1.1.1.5)
read-create
INTEGER
INTEGER
(normal, 0),
(baslocal, 6),
(basremote, 7),
(odap, 9)
IPv6 address pool type. Only 0, 6, 7, and 9 are supported.
As per the MIB.
hh3cDhcp6Server2PoolNetwork (1.3.6.1.4.1.25506.2.179.1.1.1.6)
read-create
InetAddressIPv6
OCTET STRING
(16)
Network segment in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolNetworkMask
(1.3.6.1.4.1.25506.2.179.1.1.1.7)
read-create
Integer32
Integer32 (0128)
Prefix length for the network segment in the IPv6 address pool.
If you have not configured the prefix length or remove the prefix length configuration, the prefix length is 0.
As per the MIB.
hh3cDhcp6Server2PoolNetworkPdNum (1.3.6.1.4.1.25506.2.179.1.1.1.8)
read-create
Integer32
Integer32 (01024)
Prefix number of the network segment in the IPv6 address pool.
If you have not configured the prefix number or remove the prefix number configuration, the prefix number is 0.
As per the MIB.
hh3cDhcp6Server2PoolSubPdAddr
(1.3.6.1.4.1.25506.2.179.1.1.1.9)
read-create
InetAddressIPv6
OCTET STRING
(16)
Sub-prefix of the network segment in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolSubPdLength (1.3.6.1.4.1.25506.2.179.1.1.1.10)
read-create
Integer32
Integer32 (0128)
Sub-prefix length for the network segment in the IPv6 address pool.
If you have not configured the sub-prefix length or remove the sub-prefix length configuration, the sub-prefix length is 0.
As per the MIB.
hh3cDhcp6Server2PoolNetPreTime (1.3.6.1.4.1.25506.2.179.1.1.1.11)
read-create
Unsigned32
Unsigned32 (0|604294967295)
Preferred lifetime for the network segment in the IPv6 address pool.
The default preferred lifetime is 604800 seconds.
If no network segment exists in the IPv6 address pool, the preferred lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolNetValTime
(1.3.6.1.4.1.25506.2.179.1.1.1.12)
read-create
Unsigned32
Valid lifetime for the network segment in the IPv6 address pool.
The default valid lifetime is 2592000 seconds.
If no network segment exists in the IPv6 address pool, the valid lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolNetExport
(1.3.6.1.4.1.25506.2.179.1.1.1.13)
read-create
TruthValue
true(1),
false(2)
Settings of the network routes issued for address blocks in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolNetPrefer
(1.3.6.1.4.1.25506.2.179.1.1.1.14)
read-create
Unsigned32
Unsigned32 (1255)
Preference for the network routes issued for address blocks in the IPv6 address pool. The default value is 65.
As per the MIB.
hh3cDhcp6Server2PoolNetTag
(1.3.6.1.4.1.25506.2.179.1.1.1.15)
read-create
Unsigned32
Unsigned32 (04294967295)
Tag value for the network routes issued for address blocks in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolNaStartAddr
(1.3.6.1.4.1.25506.2.179.1.1.1.16)
read-create
InetAddressIPv6
OCTET STRING
(16)
Start address of the non-temporary IPv6 address range in the IPv6 address pool for dynamic allocation.
As per the MIB.
hh3cDhcp6Server2PoolNaEndAddr (1.3.6.1.4.1.25506.2.179.1.1.1.17)
read-create
InetAddressIPv6
OCTET STRING
(16)
End address of the non-temporary IPv6 address range in the IPv6 address pool for dynamic allocation.
As per the MIB.
hh3cDhcp6Server2PoolNaPreTime (1.3.6.1.4.1.25506.2.179.1.1.1.18)
read-create
Unsigned32
Preferred lifetime for the non-temporary IPv6 addresses.
If no non-temporary IPv6 address range exists, the preferred lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolNaValTime
(1.3.6.1.4.1.25506.2.179.1.1.1.19)
read-create
Unsigned32
Valid lifetime for the non-temporary IPv6 addresses.
If no non-temporary IPv6 address range exists, the valid lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolTaStartAddr
(1.3.6.1.4.1.25506.2.179.1.1.1.20)
read-create
InetAddressIPv6
OCTET STRING
(16)
Start address of the temporary IPv6 address range in the IPv6 address pool for dynamic allocation.
As per the MIB.
hh3cDhcp6Server2PoolTaEndAddr
(1.3.6.1.4.1.25506.2.179.1.1.1.21)
read-create
InetAddressIPv6
OCTET STRING
(16)
End address of the temporary IPv6 address range in the IPv6 address pool for dynamic allocation.
As per the MIB.
hh3cDhcp6Server2PoolTaPreTime (1.3.6.1.4.1.25506.2.179.1.1.1.22)
read-create
Unsigned32
Preferred lifetime for the temporary IPv6 addresses.
If no temporary IPv6 address range exists, the preferred lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolTaValTime
(1.3.6.1.4.1.25506.2.179.1.1.1.23)
read-create
Unsigned32
Valid lifetime for the temporary IPv6 addresses.
If no temporary IPv6 address range exists, the valid lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolPrefixPool
(1.3.6.1.4.1.25506.2.179.1.1.1.24)
read-create
Integer32
Integer32 (0128)
Number of the prefix pool applied to the IPv6 address pool.
If you have not applied a prefix pool to the IPv6 address pool or remove the prefix pool configuration for the address pool, the prefix pool number is 0.
As per the MIB.
hh3cDhcp6Server2PoolPdPreTime (1.3.6.1.4.1.25506.2.179.1.1.1.25)
read-create
Unsigned32
Preferred lifetime for prefixes in the IPv6 address pool.
If no prefix pool is applied to the IPv6 address pool, the preferred lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolPdValTime
(1.3.6.1.4.1.25506.2.179.1.1.1.26)
read-create
Unsigned32
Valid lifetime for prefixes in the IPv6 address pool.
If no prefix pool is applied to the IPv6 address pool, the valid lifetime is 0 seconds.
As per the MIB.
hh3cDhcp6Server2PoolPdExport (1.3.6.1.4.1.25506.2.179.1.1.1.27)
read-create
TruthValue
true(1),
false(2)
Settings of the network routes issued for prefixes in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolPdPreference
(1.3.6.1.4.1.25506.2.179.1.1.1.28)
read-create
Unsigned32
Unsigned32 (1255)
Preference for the network routes issued for prefixes in the IPv6 address pool. The default value is 65.
As per the MIB.
hh3cDhcp6Server2PoolPdTag (1.3.6.1.4.1.25506.2.179.1.1.1.29)
read-create
Unsigned32
Tag value for the network routes issued for prefixes in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolDomainName (1.3.6.1.4.1.25506.2.179.1.1.1.30)
read-create
OCTET STRING
OCTET STRING (1..50)
Domain name specified in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolGatewayIp (1.3.6.1.4.1.25506.2.179.1.1.1.31)
read-create
OCTET STRING
OCTET STRING (1..367)
Gateway IP address specified in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolDNSIp (1.3.6.1.4.1.25506.2.179.1.1.1.32)
read-create
OCTET STRING
DNS server IP address specified in the IPv6 address pool
As per the MIB.
hh3cDhcp6Server2PoolExpireIpEnbl
(1.3.6.1.4.1.25506.2.179.1.1.1.33)
read-create
TruthValue
true(1),
false(2)
Whether to enable IPv6 address reservation in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolExpireIpMode
(1.3.6.1.4.1.25506.2.179.1.1.1.34)
read-create
INTEGER
INTEGER
(cid, 0),
(mac, 1)
IPv6 address reservation mode in the IPv6 address pool.
The default value is cid (0).
As per the MIB.
hh3cDhcp6Server2PoolExpireIpLim
(1.3.6.1.4.1.25506.2.179.1.1.1.35)
read-create
Unsigned32
Unsigned32 (1256000)
Maximum number of IPv6 addresses that can be reserved in the IPv6 address pool.
The default value is 256000.
As per the MIB.
hh3cDhcp6Server2PoolExpireIpTime
(1.3.6.1.4.1.25506.2.179.1.1.1.36)
read-create
Unsigned32
Unsigned32 (604294967295)
Reservation time for expired IPv6 addresses in the IPv6 address pool.
The default reservation time is 4294967295 seconds.
As per the MIB.
hh3cDhcp6Server2PoolExpirePdEnbl
(1.3.6.1.4.1.25506.2.179.1.1.1.37)
read-create
TruthValue
true(1),
false(2)
Whether to enable IPv6 prefix reservation in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolExpirePdMode
(1.3.6.1.4.1.25506.2.179.1.1.1.38)
read-create
INTEGER
INTEGER
(cid, 0),
(mac, 1)
IPv6 prefix reservation mode in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolExpirePdLim
(1.3.6.1.4.1.25506.2.179.1.1.1.39)
read-create
Unsigned32
Maximum number of IPv6 prefixes that can be reserved in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolExpirePdTime
(1.3.6.1.4.1.25506.2.179.1.1.1.40)
read-create
Unsigned32
Reservation time for expired IPv6 prefixes in the IPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolStatTable
About this table
Use this table to obtain DHCPv6 address pool statistics.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cDhcp6Server2PoolIPIdleNum (1.3.6.1.4.1.25506.2.179.1.2.1.1)
read-only
Unsigned32
Number of free IPv6 addresses in a DHCPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolIPUsedNum (1.3.6.1.4.1.25506.2.179.1.2.1.2)
read-only
Unsigned32
Number of assigned IPv6 addresses in the DHCPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolPrefixIdleNum (1.3.6.1.4.1.25506.2.179.1.2.1.3)
read-only
Unsigned32
Number of free IPv6 prefixes in a DHCPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolPrefixUsedNum (1.3.6.1.4.1.25506.2.179.1.2.1.4)
read-only
Unsigned32
Number of assigned IPv6 prefixes in the DHCPv6 address pool.
As per the MIB.
hh3cDhcp6Server2PoolIPTotalNum
(1.3.6.1.4.1.25506.2.179.1.2.1.5)
Read-only
OCTET STRING
Number of addresses in the DHCPv6 address pool.
hh3cDhcp6Server2PoolIPExpiredNum
(1.3.6.1.4.1.25506.2.179.1.2.1.6)
Read-only
Unsigned32
Number of expired addresses in the DHCPv6 address pool.
hh3cDhcp6Server2PoolIPDynamicUsedNum
(1.3.6.1.4.1.25506.2.179.1.2.1.7)
Read-only
Unsigned32
Number of dynamically assigned addresses in the DHCPv6 address pool.
hh3cDhcp6Server2PoolIPStaticUsedNum
(1.3.6.1.4.1.25506.2.179.1.2.1.8)
Read-only
Unsigned32
Number of statically assigned addresses in the DHCPv6 address pool.
hh3cDhcp6Server2PoolIPConflictNum
(1.3.6.1.4.1.25506.2.179.1.2.1.9)
Read-only
Counter64
Number of conflicting addresses in the DHCPv6 address pool.
hh3cDhcp6Server2PoolIPExcludeNum
(1.3.6.1.4.1.25506.2.179.1.2.1.10)
Read-only
Unsigned32
Number of excluded addresses in the DHCPv6 address pool.
hh3cDhcp6Server2PoolIPReserveNum
(1.3.6.1.4.1.25506.2.179.1.2.1.11)
Read-only
Unsigned32
Number of reserved addresses in the DHCPv6 address pool.
hh3cDhcp6Server2PoolIPUsge
(1.3.6.1.4.1.25506.2.179.1.2.1.12)
Read-only
Unsigned32
Address usage of the DHCPv6 address pool.
hh3cDhcp6Server2PoolPdTotalNum
(1.3.6.1.4.1.25506.2.179.1.2.1.13)
Read-only
OCTET STRING
Number of prefixes in the DHCPv6 address pool.
hh3cDhcp6Server2PoolPdExpiredNum
(1.3.6.1.4.1.25506.2.179.1.2.1.14)
Read-only
Unsigned32
Number of expired prefixes in the DHCPv6 address pool.
hh3cDhcp6Server2PoolPdDynamicUsedNum
(1.3.6.1.4.1.25506.2.179.1.2.1.15)
Read-only
Unsigned32
Number of dynamically assigned prefixes in the DHCPv6 address pool.
hh3cDhcp6Server2PoolPdStaticUsedNum
(1.3.6.1.4.1.25506.2.179.1.2.1.16)
Read-only
Unsigned32
Number of statically assigned prefixes in the DHCPv6 address pool.
hh3cDhcp6Server2PoolPdConflictNum
(1.3.6.1.4.1.25506.2.179.1.2.1.17)
Read-only
Unsigned32
Number of conflicting prefixes in the DHCPv6 address pool.
hh3cDhcp6Server2PoolPdExcludeNum
(1.3.6.1.4.1.25506.2.179.1.2.1.18)
Read-only
Unsigned32
Number of excluded prefixes in the DHCPv6 address pool.
hh3cDhcp6Server2PoolPdReserveNum
(1.3.6.1.4.1.25506.2.179.1.2.1.19)
Read-only
Counter64
Number of reserved prefixes in the DHCPv6 address pool.
hh3cDhcp6Server2PooPdUsage
(1.3.6.1.4.1.25506.2.179.1.2.1.20)
Read-only
Unsigned32
Prefix usage of the DHCPv6 address pool.
hh3cDhcp6Server2PoolGpTable
About this table
This table records information about DHCPv6 address pool group settings.
CreateSupported.
Edit/ModifySupported.
DeleteNot supported
ReadNot supported
Columns
The table index is hh3cDhcp6Server2PoolGpName.
Object (OID)
Access
Value range
Implementation
hh3cDhcp6Server2PoolGpName (1.3.6.1.4.1.25506.2.179.1.3.1.1)
Read-only
OCTET STRING
DHCPv6 address pool group name.
As per the MIB.
hh3cDhcp6Server2PoolGpVpnName (1.3.6.1.4.1.25506.2.179.1.3.1.2)
read-create
OCTET STRING
VPN instance to which the DHCPv6 address pool group is applied.
As per the MIB.
hh3cDhcp6Server2PoolGpIncUndo (1.3.6.1.4.1.25506.2.179.1.3.1.3)
read-write
TruthValue
Deleting all pools from the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpRowSta (1.3.6.1.4.1.25506.2.179.1.3.1.4)
read-create
RowStatus
createAndGo(4)
destroy(6)
Row status.
As per the MIB.
hh3cDhcp6Server2PoolGpExtTable
About this table
This table records DHCPv6 address pool information in a DHCPv6 address pool group.
CreateSupported.
DeleteNot supported
ReadNot supported
Columns
The table indexes are hh3cDhcp6Server2PoolGpName and hh3cDhcp6Server2PoolIndex.
Object (OID)
Access
Value range
Implementation
hh3cDhcp6Server2PoolGpIncPoolNm (1.3.6.1.4.1.25506.2.179.1.4.1.1)
read-only
OCTET STRING
As per the MIB.
hh3cDhcp6Server2PoolGpExtRowSta (1.3.6.1.4.1.25506.2.179.1.4.1.2)
read-create
RowStatus
createAndGo(4)
destroy(6)
Row status.
As per the MIB.
hh3cDhcp6Server2PoolGpStatTable
About this table
This table defines DHCPv6 address pool group statistics.
CreateNot supported.
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cDhcp6Server2PoolGpPoolNum (1.3.6.1.4.1.25506.2.179.1.5.1.1)
read-only
Unsigned32
Number of IPv6 address pools in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpBndDomNum (1.3.6.1.4.1.25506.2.179.1.5.1.2)
read-only
Unsigned32
Number of domains in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpIPUsage (1.3.6.1.4.1.25506.2.179.1.5.1.3)
read-only
Unsigned32
IPv6 address usage of the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpIPTotalNum (1.3.6.1.4.1.25506.2.179.1.5.1.4)
read-only
Unsigned32
Total number of IPv6 addresses in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpIPUsedNum
(1.3.6.1.4.1.25506.2.179.1.5.1.5)
Read-only
Unsigned32
Number of allocated IPv6 addresses in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpIPIdleNum
(1.3.6.1.4.1.25506.2.179.1.5.1.6)
Read-only
Unsigned32
Number of free IPv6 addresses in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpIPExcNum
(1.3.6.1.4.1.25506.2.179.1.5.1.7)
Read-only
Unsigned32
Number of excluded IPv6 addresses in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpIPConfNum
(1.3.6.1.4.1.25506.2.179.1.5.1.8)
Read-only
Unsigned32
Number of conflicting IPv6 addresses in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpPDUsage
(1.3.6.1.4.1.25506.2.179.1.5.1.9)
Read-only
Unsigned32
Prefix usage of the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpPDTotalNum
(1.3.6.1.4.1.25506.2.179.1.5.1.10)
Read-only
Unsigned32
Total number of prefixes in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpPDUsedNum
(1.3.6.1.4.1.25506.2.179.1.5.1.11)
Read-only
Unsigned32
Number of allocated prefixes in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpPDIdleNum
(1.3.6.1.4.1.25506.2.179.1.5.1.12)
Read-only
Unsigned32
Number of free prefixes in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpPDExcNum
(1.3.6.1.4.1.25506.2.179.1.5.1.13)
Read-only
Unsigned32
Number of excluded prefixes in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpPDConfNum
(1.3.6.1.4.1.25506.2.179.1.5.1.14)
Read-only
Unsigned32
Number of conflicting prefixes in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PoolGpIPReserveNum (1.3.6.1.4.1.25506.2.179.1.5.1.15)
Read-only
Counter64
Number of reserved IPv6 addresses in the DHCPv6 address pool group.
As per the MIB.
hh3cDhcp6Server2PrefixPoolTable
About this table
The table records the DHCPv6 prefix pool configuration parameters.
CreateSupported.
DeleteSupported
ReadSupported
Columns
The table index is hh3cDhcp6Server2PdVPNInstance and hh3cDhcp6Server2PdNumber.
Object (OID)
Access
Value range
Implementation
hh3cDhcp6Server2PdVPNInstance (1.3.6.1.4.1.25506.2.179.1.6.1.1)
not-accessible
OCTET STRING
OCTET STRING (1..31)
VPN instance bound to the prefix pool.
As per the MIB.
hh3cDhcp6Server2PdNumber (1.3.6.1.4.1.25506.2.179.1.6.1.2)
not-accessible
Integer32
Integer32(1..128)
Number of the prefix pool.
As per the MIB.
hh3cDhcp6Server2PdPrefixAddr (1.3.6.1.4.1.25506.2.179.1.6.1.3)
read-create
OCTET STRING (16)
OCTET STRING (16)
Prefix in the prefix pool.
As per the MIB.
hh3cDhcp6Server2PdPrefixLen (1.3.6.1.4.1.25506.2.179.1.6.1.4)
read-create
Integer32
Integer32(0..128)
Prefix length for the prefix above.
As per the MIB.
hh3cDhcp6Server2PdPrefixNumber (1.3.6.1.4.1.25506.2.179.1.6.1.5)
read-create
Integer32
Integer32(0..1024)
Index of the prefix applied to the prefix pool.
If no prefix is applied to the prefix pool, the index is 0.
As per the MIB.
hh3cDhcp6Server2PdPrefixAssLen (1.3.6.1.4.1.25506.2.179.1.6.1.6)
read-create
Integer32
Integer32(1..128)
Prefix length used for dynamic prefix allocation in the prefix pool.
As per the MIB.
hh3cDhcp6Server2PdRowStatus
(1.3.6.1.4.1.25506.2.179.1.6.1.7)
read-create
RowStatus
Active(1)
createAndGo(4)
destroy(6)
Row status.
As per the MIB.
Notifications
hh3cDhcp6Server2AddrExhaust
Basic information
OID
Event
Severity
Recovery notification
Default status
1.3.6.1.4.1.25506.2.179.2.0.1
Addresses in an IPv6 address pool have been exhausted.
Error
Major
1.3.6.1.4.1.25506.2.179.2.0.2 (hh3cDhcp6Server2AddrExhaustRecov)
ON
Notification triggers
This notification is generated when all addresses in an IPv6 address pool are assigned.
System impact
New DHCPv6 users cannot obtain IPv6 addresses from the DHCPv6 server.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server address-exhaust command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server address-exhaust command.
Object
OID (object name)
Index
Value range
1.3.6.1.4.1.25506.2.179.1.1.1.1 (hh3cDhcp6Server2PoolIndex)
IPv6 address pool index.
Unsigned32
Recommended action
To resolve this issue:
1.Use one of the following methods to increase address resources:
  - Add the current address pool and other address pools to an address pool group.
  - Add secondary network segments for dynamic address allocation in the current address pool.
If the issue persists, proceed to step 2.
2.If the issue persists, collect alarm information, log messages, and configuration data, and then contact H3C Support for help.
Basic information
OID
Event
Severity
Default status
An IPv6 address pool has recovered from address exhaustion.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when an IPv6 address pool has recovered from address exhaustion.
System impact
No negative impact on the system.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
No action is required.
hh3cDhcp6Server2IpUsageOverflow
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.3
The address usage of an IPv6 address pool has exceeded the threshold.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.4 (hh3cDhcp6Server2IpUsageOverflowRecov)
ON
This notification is generated when the address usage of an IPv6 address pool has exceeded the threshold.
System impact
If the DHCPv6 server continues to assign IPv6 addresses from the address pool to clients, the address pool might run out of addresses. As a result, new DHCPv6 users cannot obtain IPv6 addresses and thus cannot come online.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server ip-in-use command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server ip-in-use command.
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
1.Use the display ipv6 pool command in any view to check whether the address usage threshold specified in the current address pool is appropriate.
  - If the address usage threshold is too low, increase the threshold.
  - If the address usage threshold is appropriate, proceed to step 2.
2.Use the display ipv6 dhcp server statistics command in any view to view the address usage of the current address pool and the number of assignable addresses in the current address pool.
  - If the assignable addresses are insufficient, replan and increase address pool resources. For example, you can increase address resources as follows:
  - i. Use the ipv6 pool-group command to create an IPv6 address pool group, and then add multiple address pools to the address pool group.
  - ii. Use the undo authorization-attribute ipv6-pool command in ISP domain view to remove the current authorization IPv6 address pool attribute.
  - iii. Use the authorization-attribute ipv6-pool-group command in ISP domain view to specify the IPv6 address pool group for users.
  - If the assignable addresses are sufficient, keep observing the address usage of the current address pool. When the address pool has a high address usage, increase address resources timely to ensure that new DHCPv6 users can obtain addresses.
3.If the issue persists, collect alarm information, log messages, and configuration data, and then contact H3C Support for help.
Basic information
OID
Event
Severity
Default status
The address usage of an IPv6 address pool has dropped below the threshold.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the address usage of an IPv6 address pool has dropped below the threshold.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
hh3cDhcp6Server2PdExhaust
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.5
Prefixes in an IPv6 address pool have been exhausted.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.6 (hh3cDhcp6Server2PdExhaustRecov)
ON
This notification is generated when all prefixes in an IPv6 address pool are assigned.
System impact
New DHCPv6 users cannot come online.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server pd-exhaust command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server pd-exhaust command.
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
1.Replan and increase address pool resources. For example, you can increase address resources as follows:
Basic information
OID
Event
Severity
Default status
An IPv6 address pool has recovered from prefix exhaustion.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when an IPv6 address pool has recovered from prefix exhaustion.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
hh3cDhcp6Server2PdUsageOverflow
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.7
The prefix usage of an IPv6 address pool has reached or exceeded the threshold.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.8 (hh3cDhcp6Server2PdUsageOverflowRecov)
ON
This notification is generated when the prefix usage of an IPv6 address pool has reached or exceeded the threshold.
System impact
If the number of DHCPv6 users keeps increasing, the IPv6 address pool might run out of prefix resources. As a result, new DHCPv6 users cannot come online.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server pd-in-use command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server pd-in-use command.
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
1.Use the display ipv6 pool command in any view to check whether the prefix usage threshold specified in the current address pool is appropriate.
  - If the prefix usage threshold is too low, increase the threshold.
  - If the prefix usage threshold is appropriate, proceed to step 2.
2.Use the display ipv6 dhcp server statistics command in any view to view the prefix usage of the current address pool and the number of assignable prefixes in the current address pool.
  - If the assignable prefixes are insufficient, replan and increase address pool resources. For example, you can increase address resources as follows:
  - If the assignable prefixes are sufficient, keep observing the prefix usage of the current address pool. When the address pool has a high prefix usage, increase prefix resources timely to ensure that new DHCPv6 users can obtain prefixes.
hh3cDhcp6Server2IpNetUsageOverflow
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.9
The subnet usage of an IPv6 address pool has reached or exceeded the threshold.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.10 (hh3cDhcp6Server2IpNetUsageOverflowRecov)
ON
This notification is generated when the subnet usage of an IPv6 address pool has reached or exceeded the threshold.
System impact
If the DHCPv6 server continues to assign addresses from the subnet to clients, the subnet might run out of addresses. As a result, new DHCPv6 users cannot obtain IPv6 addresses and thus cannot come online.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
1.Use the display ipv6 dhcp dynamic address command in any view to view the subnets in IPv6 address pools that support dynamic IPv6 subnet allocation.
If the utilization of each subnet is high, use the dynamic utilization mark command to adjust the low utilization mark. This operation will make corresponding address pools to release idle subnets.
If the utilization of each subnet is not high, keep observing the utilization of each subnet. When the subnet utilization is high, increase subnet resources timely to ensure that new DHCPv6 users can obtain addresses.
Basic information
OID
Event
Severity
Default status
The subnet usage of an IPv6 address pool has dropped below the threshold.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the subnet usage of an IPv6 address pool has dropped below the threshold.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
hh3cDhcp6Server2IpNetExhaust
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.11
Subnets in an IPv6 address pool have been exhausted.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.12 (hh3cDhcp6Server2IpNetExhaustRecov)
ON
This notification is generated when an IPv6 address pool has run out of subnet resources.
System impact
DHCPv6 users might fail to come online.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
1.Use the display ipv6 dhcp dynamic address command in any view to view the address usage of subnets in the current IPv6 address pool.
If the address usage of each subnet is high, use the dynamic utilization mark command to adjust the low utilization mark. This operation will make corresponding address pools to release idle subnets.
Basic information
OID
Event
Severity
Default status
An IPv6 address pool has recovered from subnet exhaustion.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when an IPv6 address pool has recovered from subnet exhaustion.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
hh3cDhcp6Server2PdNetUsageOverflow
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.13
The prefix sub-range usage of an IPv6 address pool has reached or exceeded the threshold.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.14 (hh3cDhcp6Server2PdNetUsageOverflowRecov)
ON
This notification is generated when the prefix sub-range usage of an IPv6 address pool has reached or exceeded the threshold.
System impact
If the DHCPv6 server continues to assign prefix sub-ranges from the IPv6 address pool, the IPv6 address pool might run out of prefix sub-range resources. As a result, new DHCPv6 users cannot obtain IPv6 addresses and thus cannot come online.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
1.Use the display ipv6 dhcp dynamic prefix command in any view to view the prefix usage of prefix ranges in the current IPv6 address pool.
If the prefix usage of prefix range is high, use the dynamic utilization mark command to adjust the low utilization mark. This operation will make corresponding address pools to release idle prefix ranges.
hh3cDhcp6Server2PdNetExhaust
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.15
Prefix sub-ranges in the IPv6 address pool have been exhausted.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.16 (hh3cDhcp6Server2PdNetExhaustRecov)
ON
This notification is generated when prefix sub-ranges in an IPv6 address pool have been exhausted.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
1.Use the display ipv6 pool-group command in any view and view the IPv6 pool group pd usage field in the command output. Then, determine whether to add more usable prefixes. If yes, proceed to step 2.
2.Use the pool command in IPv6 address pool group view to add usable address pools to the address pool group.
If the issue persists, proceed to step 3.
3.Collect alarm information, log messages, and configuration data, and then contact H3C Support for help.
Basic information
OID
Event
Severity
Default status
An IPv6 address pool has recovered from prefix sub-range exhaustion.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when an IPv6 address pool has recovered from prefix sub-range exhaustion.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Unsigned32
Recommended action
hh3cDhcp6Server2GpIpNetExhaust
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.17
Subnets in an IPv6 address pool group have been exhausted.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.18 (hh3cDhcp6Server2GpIpNetExhaustRecov)
ON
This notification is generated when subnets in an IPv6 address pool group have been exhausted.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
1.3.6.1.4.1.25506.2.179.1.3.1.1 (hh3cDhcp6Server2PoolGpName)
Name of the IPv6 address pool group.
OCTET STRING
Recommended action
If more usable prefixes are required, proceed to step 2.
Basic information
OID
Event
Severity
Default status
An IPv6 address pool group has recovered from subnet exhaustion.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when an IPv6 address pool group has recovered from subnet exhaustion.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
OCTET STRING
Recommended action
hh3cDhcp6Server2GpPdNetExhaust
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.19
Prefix ranges in an IPv6 address pool group have been exhausted.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.20 (hh3cDhcp6Server2GpPdNetExhaustRecov)
ON
This notification is generated when prefix ranges in an IPv6 address pool group have been exhausted.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
OCTET STRING
Recommended action
2.Use the pool command in IPv6 address pool group view to add address pools with usable prefixes to the address pool group.
Basic information
OID
Event
Severity
Default status
An IPv6 address pool group has recovered from prefix range exhaustion.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when an IPv6 address pool group has recovered from prefix range exhaustion.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
OCTET STRING
Recommended action
hh3cDhcp6Svr2AllocIpFailed
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.21
The DHCPv6 server fails to allocate an IPv6 address in an ISP domain.
Informational
Warning
N/A (N/A)
ON
This notification is generated when the DHCPv6 server fails to allocate an IPv6 address in an ISP domain.
System impact
Access users cannot obtain IPv6 addresses from the ISP domain.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcpserver ip-alloc-failed command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcpserver ip-alloc-failed command.
Object
OID (object name)
Index
Value range
1.3.6.1.4.1.25506.2.179.3.1.1 (hh3cDhcp6Server2OnlineFailReason)
Reason for the address allocation failure on the DHCPv6 server.
N/A
OCTET STRING
Recommended action
1.Use the display domain command in any view to check whether the authorization-attribute ipv6-pool command is configured.
  - If the command is configured, verify that the access configuration is correct. For more information about this task, see IPoE configuration in Layer 2—WAN Access Configuration Guide.
  - If the command is not configured, proceed to step 2.
2.Use the display ipv6 dhcp server statistics command in any view and check whether the value of the Free IPv6 addresses field is 0 in the command output.
If the value of the Free IPv6 addresses field is 0, perform the following task to increase usable address pool resources:
hh3cDhcp6Svr2AllocPdFailed
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.22
The DHCPv6 server fails to allocate an IPv6 prefix in an ISP domain.
Informational
Warning
N/A (N/A)
ON
This notification is generated when the DHCPv6 server fails to allocate an IPv6 prefix in an ISP domain.
System impact
Access users cannot obtain IPv6 prefixes from the ISP domain.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server pd-alloc-failed command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server pd-alloc-failed command.
Object
OID (object name)
Index
Value range
Reason for the prefix allocation failure on the DHCPv6 server.
N/A
OCTET STRING
Recommended action
If the value of the Free IPv6 prefixes field is 0, perform the following task to increase usable address pool resources:
hh3cDhcp6Svr2GpAddrExhaust
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.24
An address pool group has run out of IPv6 addresses.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.25 (hh3cDhcp6Svr2GpAddrExhaustRecov)
ON
This notification is generated when an IPv6 address pool group has run out of IPv6 addresses.
System impact
DHCPv6 users cannot obtain addresses and thus cannot come online.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server group-used-exhaustion command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server group-used-exhaustion command.
Object
OID (object name)
Index
Value range
Name of the address pool group.
Recommended action
1.Use the display ipv6 pool-group command in any view and view the Pool group address usage field in the command output. Then, determine whether to add more usable addresses. If yes, proceed to step 2.
Basic information
OID
Event
Severity
Default status
An IPv6 address pool group has recovered from the address resource exhaustion condition.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when an IPv6 address pool group has recovered from the address resource exhaustion condition.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Recommended action
hh3cDhcp6Server2DevOdapFull
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.26
All ODAP address pools have run out of subnet resources.
Informational
Warning
N/A (N/A)
ON
This notification is generated when all ODAP address pools have run out of subnet resources.
System impact
New DHCPv6 users might fail to come online.
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server odap-subnet-warning command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server odap-subnet-warning command.
Object
OID (object name)
Index
Value range
N/A (N/A)
N/A
N/A
N/A
N/A
Recommended action
1.Use the display ipv6 dhcp dynamic address command in any view to view the address usage of subnets in ODAP address pools.
hh3cDhcp6Server2DevOdapPdFull
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.27
All ODAP address pool have run out of prefix range resources.
Informational
Warning
N/A (N/A)
ON
This notification is generated when all ODAP address pools have run out of prefix range resources.
System impact
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server odap-prefix-warning command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server odap- prefix-warning command.
Object
OID (object name)
Index
Value range
N/A (N/A)
N/A
N/A
N/A
N/A
Recommended action
1.Use the display ipv6 dhcp dynamic prefix command in any view to view the prefix usage of prefix ranges in ODAP address pools.
If the prefix usage of each prefix range is high, use the dynamic utilization mark command to adjust the low utilization mark. This operation will make corresponding address pools to release idle subnets.
hh3cDhcp6Server2OdapApplyFail
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.28
An ODAP address pool fails to request subnet resources.
Informational
Warning
N/A (N/A)
ON
This notification is generated when one of the following conditions exists:
The ODAP server does not respond to the subnet request.
The ODAP server is configured incorrectly.
The ODAP server has run out of subnet resources.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Reason why the ODAP address pool failed to request subnet resources.
N/A
OCTET STRING
Recommended action
1.Verify that the ODAP settings are all correct. If the ODAP settings are configured correctly, proceed to step 2.
2.Use the display ipv6 dhcp dynamic-alloc address command to check whether the utilization of each subnet is normal in the ODAP address pool.
hh3cDhcp6Server2OdapReleaseFail
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.29
An ODAP address pool fails to release subnet resources.
Informational
Warning
N/A (N/A)
ON
This notification is generated when the device is disconnected from the ODAP server.
System impact
This issue might disable the ODAP server from reclaiming subnets and the ODAP server might run out of subnet resources.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Reason why the ODAP address pool failed to release subnet resources.
N/A
OCTET STRING
Recommended action
hh3cDhcp6Server2OdapApplyPdFail
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.30
An ODAP address pool fails to request prefix range resources.
Informational
Warning
N/A (N/A)
ON
System impact
Status control
ON
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server odap-prefix-warning command.
Object
OID (object name)
Index
Value range
Reason why the ODAP address pool failed to request prefix range resources.
N/A
OCTET STRING
Recommended action
hh3cDhcp6Server2OdapReleasePdFail
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.31
An ODAP address pool fails to release prefix range resources.
Informational
Warning
N/A (N/A)
ON
This notification is generated when an ODAP address pool fails to release prefix range resources.
System impact
This issue might disable the ODAP server from reclaiming prefix range resources and the ODAP server might run out of prefix range resources.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Reason why the ODAP address pool failed to release prefix range resources.
N/A
OCTET STRING
Recommended action
hh3cDhcp6Svr2GpUsageOverflow
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.179.2.0.32
The IPv6 resource usage of an address pool group has reached the threshold.
Error
Warning
1.3.6.1.4.1.25506.2.179.2.0.33 (hh3cDhcp6Svr2GpUsageOverflowRecov)
ON
This notification is generated when the IPv6 resource usage of an address pool group has reached the threshold.
System impact
The address pool group might run out of IPv6 address and prefix resources. As a result, new DHCPv6 users might fail to come online.
Status control
ON
CLI: Use the snmp-agent trap enable dhcp server group-used-threshold command.
OFF
CLI: Use the undo snmp-agent trap enable dhcp server group-used-threshold command.
Object
OID (object name)
Index
Value range
Recommended action
1.Use the display ipv6 pool-group command in any view and view the address usage field in the command output. Then, determine whether more usable addresses are required. To add more usable addresses, proceed to step 2.
Basic information
OID
Event
Severity
Default status
The IPv6 resource usage of an address pool group has dropped below the threshold.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the IPv6 resource usage of an address pool group has dropped below the threshold.
System impact
Status control
ON
CLI: Use the snmp-agent trap enable ipv6 dhcp server group-used-threshold command.
OFF
CLI: Use the undo snmp-agent trap enable ipv6 dhcp server group-used-threshold command.
Object
OID (object name)
Index
Value range
Recommended action
