1 Product models and technical specifications

Product models

H3C S9820-8C switches are high-density intelligent 100G/400G switches developed for data centers, providing powerful hardware forwarding capacity and abundant data center features.

This document is applicable to H3C S9820-8C switch (product code: LS-9820-8C).

Technical specifications

Table1-1 Technical specifications

Item

Specification

Dimensions (H × W × D)

130.5 × 440 × 760 mm (5.14 × 17.32 × 29.92 in)

Weight (fully configured with fan trays and power modules, excluding transceiver modules and cables)

≤ 45 kg (99.21 lb)

Console port

·     1 × mini USB console port

·     1 × serial console port

Management Ethernet port

·     1 × 10/100/1000BASE-T copper port

·     1 × SFP port

USB port

1

Power module slot

4

Interface module slot

8

Fan tray slot

5

Minimum power consumption

305 W

For the conditions under which the minimum power consumption is collected, see Table1-2.

Typical power consumption

·     Configured with LSWM116H interface modules: 921 W

·     Configured with LSWM1M4CD interface modules: 820 W

For the conditions under which the typical power consumption is collected, see Table1-2.

Maximum power consumption

·     Configured with LSWM116H interface modules: 1818 W

·     Configured with LSWM1M4CD interface modules: 1655 W

For the conditions under which the maximum power consumption is collected, see Table1-2.

Chassis leakage current compliance

·     UL60950-1

·     EN60950-1

·     IEC60950-1

·     GB4943.1

Sound pressure level at 27°C (80.6°F)

65.6 dB(A)

Operating altitude

–60 m to +5000 m (–196.85 ft to +16404.20 ft)

Operating temperature

0°C to 45°C (32°F to 113°F)

Note:

The allowed maximum temperature decreases by 0.33 °C (32.59°F) as the altitude increases by 100 m (328.08 ft) from 0 m (0 ft).

Operating humidity

5% RH to 95% RH, noncondensing

Storage altitude

–60 m to +5000 m (–196.85 ft to +16404.20 ft)

Storage temperature

–40°C to +70°C (–40°F to +158°F)

Storage humidity

5% RH to 95% RH, noncondensing

Fire resistance compliance

·     UL60950-1

·     EN60950-1

·     IEC60950-1

·     GB4943.1

 

Table1-2 Power consumption collection conditions

Item

Minimum power consumption

Typical power consumption

Maximum power consumption

Configuration

·     Two power modules.

·     No transceiver modules or cables connected to the ports.

·     Two power modules.

·     Fully configured with copper cables.

·     Two power modules.

·     Fully configured with transceiver modules.

Load

No

50% load

100% load

 


2 Chassis views

Figure2-1 Front panel

(1) Interface module 1

(2) Interface module 2

(3) Interface module 3

(4) Interface module 4

(5) Interface module 5

(6) Interface module 6

(7) Interface module 7

(8) Interface module 8

 

Figure2-2 Rear panel

(1) Fiber management Ethernet port (numbered 1)

(2) Grounding point

(3) Copper management Ethernet port (numbered 0)

(4) Serial console port

(5) Mini USB console port

(6) USB port

(7) Serial label pull tab

(8) Power module 1

(9) Power module 2

(10) Power module 3

(11) Power module 4

(12) Fan tray 5

(13) Fan tray 4

(14) Fan tray 3

(15) Fan tray 2

(16) Fan tray 1

(17) System status LED (SYS)

(18) Copper management Ethernet port LED (LINK/ACT)

(19) Fiber management Ethernet port LED (LINK/ACT)

 

The ESN serial number and MAC address of the switch can be found on the serial label pull tab.

The switch came with power module slots PWR1 and PWR2 empty and power module slots PWR3 and PWR4 each installed with a filler panel. You can install two to four power modules for the switch as needed. In Figure2-2, PSR1600B-12A-B power modules are installed in the four power module slots.

The switch came with the five fan tray slots empty. You must install five fan trays of the same model for the switch. In Figure2-2, FAN-80B-1-B fan trays are installed in the five fan tray slots.

The switch came with the eight interface module slots each installed with a filler panel. You can install one to eight interface modules for the switch as needed. In Figure2-1, LSWM116H interface modules are installed in the eight interface module slots.

The switch supports shipping with fan trays and power modules installed. To purchase a switch preinstalled with fans trays and power modules, contact marketing staff.


3 FRUs

The switch uses modular design and supports the following removable components:

·     PSR1600B-12A-B power module

·     FAN-80B-1-B fan tray

·     LSWM116H interface module

·     LSWM1M4CD interface module

 

说明: IMPORTANT

IMPORTANT:

For interface module compatibility with software releases, see the release notes.

 

Power modules

说明: WARNING

WARNING!

When the switch has power modules in redundancy, you can replace a power module without powering off the switch. To avoid device damage and personal injury, make sure the power module is powered off before you replace it.

 

The switch can operate correctly with two power modules. You can install three or four power modules on the switch for 2+1 or 2+2 redundancy, respectively.

Table3-1 Power module specifications

Power module model

Specifications

Remarks

PSR1600B-12A-B

·     Rated AC input voltage: 100 VAC to 240 VAC @ 50 Hz or 60 Hz

·     Max AC input voltage: 90 VAC to 290 VAC @ 47 Hz to 63 Hz

·     Rated HVDC input voltage: 240 VDC

·     Max HVDC input voltage: 180 VDC to 320 VDC

·     Max output power: 1600 W

·     Melting current of the power module fuse: 10 A/250 V

For more information about the power module, see H3C PSR1600B-12A-B Power Module User Manual.

 

Fan trays

说明: CAUTION

CAUTION:

For adequate heat dissipation, you must install five fan trays of the same model for the switch.

 

Table3-2 Fan tray specifications

Fan tray model

Item

Specifications

FAN-80B-1-B

Dimensions (including the handle)

84 × 81 × 240 mm (3.31 × 3.19 × 9.45 in)

Fan speed

12800 R.P.M

Maximum airflow

130 CFM (3.68 m3/min)

Maximum power consumption

102 W

Documentation reference

H3C FAN-80B-1-B Fan tray User Guide

 

Interface modules

The switch provides eight interface module slots. Table3-3 describes the interface modules available for the switch.

Table3-3 Available interface modules

Model

Description

Port type and number

Available transceiver modules and cables

LSWM116H

16-port QSFP28 Ethernet optical interface module

16 × QSFP28 ports

See "QSFP28 port."

LSWM1M4CD

4-port 400GBASE Ethernet optical interface module(QSFP-DD)

4 × QSFP-DD ports

See "QSFP-DD port."

 

Table3-4 Interface module specifications

Model

Dimensions (H × W × D)

Weight (with no transceiver modules or cables)

Minimum power consumption

Typical power consumption

Maximum power consumption

LSWM116H

50 × 127.3 × 262.2 mm (1.97 × 5.01 × 10.32 in)

1.4 kg (3.09 lb)

32 W

52 W

87 W

LSWM1M4CD

50 × 127.3 × 262.2 mm (1.97 × 5.01 × 10.32 in)

1.3 kg (2.87 lb)

26 W

39 W

87 W

 

 

NOTE:

Interface module dimensions are expressed as follows:

·     H—Height of the front panel of the interface module.

·     W—Width of the front panel of the interface module.

·     D—Depth from the front panel of the interface module to the connector end (excluding the ejector lever).

 


4 Ports and LEDs

As a best practice, use H3C transceiver modules and cables for the switch. H3C transceiver modules and cables are subject to change over time. For the most up-to-date list of H3C transceiver modules and cables, contact H3C Support or marketing staff.

For information about the specifications of H3C transceiver modules and cables, see H3C Transceiver Modules User Guide.

The switch uses high-power ports in high density. Bringing up the ports simultaneously takes a comparatively long time. To reduce the time to bring up a port, the system does not turn off the laser transmitter on the transceiver module when shutting down the port.

Ports

Console port

The switch has a serial console port and a mini USB console port.

Table4-1 Console port specifications

Item

Serial console port

Mini USB console port

Connector type

RJ-45

USB mini-Type B

Compliant standard

EIA/TIA-232

USB 2.0

Transmission baud rate

9600 bps (default) to 115200 bps

Services

·     Provides connection to an ASCII terminal.

·     Provides connection to the serial port of a local terminal (a PC for example) or remote terminal (through a pair of modems) running a terminal emulation program.

·     Provides connection to an ASCII terminal.

·     Provides connection to the USB port of a local terminal (a PC for example) running a terminal emulation program.

 

Management Ethernet port

The switch has two management Ethernet ports: a copper management port and an SFP management port. You can connect the ports to a local PC for software loading and debugging or to a remote management station for remote management.

Table4-2 Management Ethernet port specifications

Item

Specification

Connector type

·     10/100/1000BASE-T management port: RJ-45.

·     SFP management port: LC.

Port transmission rate, duplex mode, and auto MDI/MDI-X

·     10/100/1000BASE-T management port:

¡     10/100 Mbps, half/full duplex, auto MDI/MDI-X.

¡     1000 Mbps, full duplex, auto MDI/MDI-X.

·     SFP management port: 1000/100 Mbps, full duplex.

Transmission medium and max transmission distance

·     10/100/1000BASE-T management port: 100 m (328.08 ft) over category-5 UTP cable.

·     SFP management port: See FE SFP transceiver modules in Table4-3 and GE SFP transceiver modules in Table4-4.

Functions and services

Software upgrade and network management.

 

Table4-3 FE SFP transceiver modules available for the SFP management port

FE SFP transceiver module

Central wavelength (nm)

Connector

Fiber type and diameter (µm)

Max transmission distance

SFP-FE-SX-MM1310-A

1310

LC

Multi-mode, 50/125

2 km (1.24 miles)

Multi-mode, 62.5/125

SFP-FE-LX-SM1310-A

1310

LC

Single-mode, 9/125

15 km (9.32 miles)

SFP-FE-LH40-SM1310

1310

LC

Single-mode, 9/125

40 km (24.86 miles)

 

Table4-4 GE SFP transceiver modules available for the SFP management port

GE SFP transceiver module

Central wavelength (nm)

Connector

Cable/Fiber type and diameter (µm)

Modal bandwidth (MHz × km)

Max transmission distance

SFP-GE-T

N/A

RJ-45

Twisted pair cable

N/A

100 m (328.08 ft)

SFP-GE-SX-MM850-A

850

LC

Multi-mode, 50/125

500

550 m (1804.46 ft)

400

500 m (1640.42 ft)

Multi-mode, 62.5/125

200

275 m (902.23 ft)

160

200 m (656.17 ft)

SFP-GE-LX-SM1310-A

1310

LC

Single-mode, 9/125

N/A

10 km (6.21 miles)

Multi-mode, 50/125

500 or 400

550 m (1804.46 ft)

Multi-mode, 62.5/125

500

550 m (1804.46 ft)

SFP-GE-LH40-SM1310

1310

LC

Single-mode, 9/125

N/A

40 km (24.86 miles)

SFP-GE-LH40-SM1550

1550

LC

Single-mode, 9/125

N/A

40 km (24.86 miles)

SFP-GE-LH80-SM1550

1550

LC

Single-mode, 9/125

N/A

80 km (49.71 miles)

 

USB port

The switch has one OHCI-compliant USB 2.0 port that can upload and download data at a rate up to 480 Mbps. You can use this USB port to access the file system on the flash of the switch, for example, to upload or download application and configuration files.

The USB port supplies power as per USB 2.0 specifications. Use only USB 2.0-compliant USB devices for the USB port. The port might not identify USB devices that are not compliant with USB 2.0.

 

 

NOTE:

USB devices from different vendors vary in compatibilities and drivers. H3C does not guarantee correct operation of USB devices of all vendors on the switch. If a USB device fails to operate on the switch, replace it with one from another vendor.

 

QSFP28 port

The LSWM116H interface module provides 16 QSFP28 ports and does not support splitting a QSFP28 port into four breakout interfaces.

The following transceiver modules and cables are available for the QSFP28 ports:

·     QSFP28 transceiver modules in Table4-5.

·     QSFP28 copper cables in Table4-6.

·     QSFP28 fiber cables in Table4-7.

·     QSFP+ transceiver modules in Table4-8.

·     QSFP+ copper cables in Table4-9.

·     QSFP+ fiber cables in Table4-10.

Table4-5 QSFP28 transceiver modules available for the QSFP28 ports

QSFP28 transceiver module

Central wavelength (nm)

Connector

Fiber type and diameter (µm)

Modal bandwidth (MHz*km)

Maximum transmission distance

QSFP-100G-SR4-MM850

850

MPO (PC polished, 12-fiber)

Multi-mode, 50/125

2000

70 m (229.66 ft)

4700

100 m (328.08 ft)

QSFP-100G-PSM4-SM1310

1295 to 1325

MPO (APC polished, 12-fiber)

Single-mode, 9/125

N/A

0.5 km (0.31 miles)

QSFP-100G-LR4L-WDM1300

Four lanes:

·     1264.5 to 1277.5

·     1284.5 to 1297.5

·     1304.5 to 1317.5

·     1324.5 to 1337.5

LC

Single-mode, 9/125

N/A

2 km (1.24 miles)

 

Table4-6 QSFP28 copper cables available for the QSFP28 ports

QSFP28 copper cable

Cable length

QSFP-100G-D-CAB-1M

1 m (3.28 ft)

QSFP-100G-D-CAB-3M

3 m (9.84 ft)

QSFP-100G-D-CAB-5M

5 m (16.40 ft)

 

Table4-7 QSFP28 fiber cables available for the QSFP28 ports

QSFP28 fiber cable

Cable length

QSFP-100G-D-AOC-7M

7 m (22.97 ft)

QSFP-100G-D-AOC-10M

10 m (32.81 ft)

QSFP-100G-D-AOC-20M

20 m (65.62 ft)

 

Table4-8 QSFP+ transceiver modules available for the QSFP28 ports

QSFP+ transceiver module

Central wavelength (nm)

Connector

Fiber type and diameter (µm)

Modal bandwidth (MHz × km)

Max transmission distance

QSFP-40G-SR4-MM850

850

MPO (PC-polished, 12-core)

Multi-mode, 50/125

2000

100 m (328.08 ft)

4700

150 m (492.12 ft)

QSFP-40G-CSR4-MM850

850

MPO (PC-polished, 12-core)

Multi-mode, 50/125

2000

300 m (984.25 ft)

4700

400 m (1312.33 ft)

QSFP-40G-BIDI-SR-MM850

850

LC

Multi-mode, 50/125

2000

100 m (328.08 ft)

4700

150 m (492.12 ft)

QSFP-40G-LR4-WDM1300

Four lanes:

·     1271

·     1291

·     1311

·     1331

LC

Single-mode, 9/125

N/A

10 km (6.21 miles)

QSFP-40G-LR4L-WDM1300

Four lanes:

·     1271

·     1291

·     1311

·     1331

LC

Single-mode, 9/125

N/A

2 km (1.24 miles)

QSFP-40G-ER4-WDM1300

Four lanes:

·     1271

·     1291

·     1311

·     1331

LC

Single-mode, 9/125

N/A

40 km (24.86 miles)

 

Table4-9 QSFP+ copper cables available for the QSFP28 ports

QSFP+ copper cable

Max transmission distance

LSWM1QSTK0

1 m (3.28 ft)

LSWM1QSTK1

3 m (9.84 ft)

LSWM1QSTK2

5 m (16.40 ft)

 

Table4-10 QSFP+ fiber cables available for the QSFP28 ports

QSFP+ fiber cable

Cable length

QSFP-40G-D-AOC-7M

7 m (22.97 ft)

QSFP-40G-D-AOC-10M

10 m (32.81 ft)

QSFP-40G-D-AOC-20M

20 m (65.62 ft)

 

 

NOTE:

MPO connectors include physical contact (PC) connectors with a flat-polished face and angle-polished contact (APC) connectors with an angle-polished face (8°).

 

QSFP-DD port

The LSWM1M4CD interface module provides 4 QSFP-DD ports.

The QSFP-DD transceiver modules are available for the QSFP-DD ports.

Table4-11 QSFP-DD transceiver modules available for the QSFP-DD ports

QSFP-DD transceiver module

Central wavelength (nm)

Connector

Fiber type and diameter (µm)

Modal bandwidth (MHz*km)

Maximum transmission distance

QSFPDD-400G-SR8-MM850

850

MPO (APC polished, 16-fiber)

50/125 µm MMF

2000

70 m (229.66 ft)

4700

100 m (328.08 ft)

 

LEDs

System status LED

The system status LED shows the operating status of the switch.

Table4-12 System status LED description

LED mark

Status

Description

SYS

Steady green

The switch is operating correctly.

Flashing green

The switch is performing power-on self-test (POST).

Steady red

The system has failed to pass POST or a fault has occurred.

Flashing blue (3 Hz)

Helps identifying the switch.

To identify the switch location, execute the locator blink blink-time command. This LED will flash blue at 3 Hz.

Off

The switch is powered off or has failed to start up.

 

QSFP28 port LED

Table4-13 QSFP28 port LED description

LED status

Description

Steady green

A transceiver module or cable has been correctly installed in the port. The port has a link and is operating at 100 Gbps.

Flashing green

The port is sending or receiving data at 100 Gbps.

Steady yellow

A transceiver module or cable has been correctly installed in the port. The port has a link and is operating at 40 Gbps.

Flashing yellow (3 Hz)

The port is sending or receiving data at 40 Gbps.

Off

No transceiver module or cable has been installed in the port, or no link is present on the port.

 

QSFP-DD port LED

Table4-14 QSFP-DD port LED description

LED status

Description

Steady green

A transceiver module is installed in the port. The port is operating at its maximum speed of 400 Gbps, and a link is present on the port.

Flashing green

The port is sending or receiving data at its maximum speed of 400 Gbps.

Steady yellow

A transceiver module is installed in the port. The port is operating at a speed lower than the maximum speed.

Flashing yellow (3 Hz)

The port is sending or receiving data at a speed lower than the maximum speed.

Off

No transceiver module is installed in the port, or no link is present on the port.

 

Management Ethernet port LEDs

The switch provides a LINK/ACT LED for each management Ethernet port to indicate their operating status.

Table4-15 Management Ethernet port LED description

LED mark

Status

Description

LINK/ACT

Off

No link is present on the port.

Steady green

The port is operating at 1000 Mbps.

Flashing green

The port is receiving or sending data at 1000 Mbps.

Steady yellow

The port is operating at 100 Mbps.

Flashing yellow

The port is receiving or sending data at 100 Mbps.

 

Power module alarm LED

A PSR1600B-12A-B power module provides an alarm LED.

Table4-16 Description for the alarm LED on a PSR1600B-12A-B power module

Status

Description

Steady green

The power module is operating correctly and in active state.

Flashing green at 1 Hz

The power module is operating correctly and in standby state.

Flashing green at 2 Hz

The power module software is being upgraded.

Steady amber

The power module is faulty or has entered self-protection mode.

Flashing amber at 1 Hz

An alarm has occurred on the power module.

Flashing amber at 2 Hz

The power module does not have input power but the power modules working in parallel with it have input power.

Off

Neither this power module nor power modules working in parallel with it have input power.

 

Fan tray alarm LED

A FAN-80B-1-B fan tray provides an alarm LED.

Table4-17 Description for the alarm LED on a FAN-80B-1-B fan tray

Status

Description

Steady green

The fan tray is operating correctly.

Steady red

The fan tray is faulty.

Off

The fan tray is operating correctly or no power is present.

 


5 Cooling system

说明: CAUTION

CAUTION:

The chassis and power modules use separate air aisles. Make sure the two aisles are not blocked when the switch is operating.

 

The switch uses a highly efficient front-rear air aisle cooling system to ensure adequate heat dissipation and improve system reliability. Consider the ventilation design at the installation site when you plan the installation location for the switch.

Table5-1 Fan tray options for the switch

Available fan tray

Airflow direction of the chassis

FAN-80B-1-B

From the port side to the power module side

 

Figure5-1 Airflow from the port side to the power module side (with FAN-80B-1-B fan trays)

 


6 Cable routing recommendations

You can purchase one cable management frame for the switch and install it on the rack posts immediately above or below the switch as required. For more organized cabling, you can purchase two cable management frames so that the switch has a cable management frame installed both above and below it.

Route the signal cables along the left or right side of the cable management frame as required. Cable routing in Figure6-1 is for your reference.

Figure6-1 Cable routing

 

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
All Support
  • Become a Partner
  • Partner Resources
  • Partner Business Management
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us
新华三官网