11-Network Management and Monitoring Command Reference
HomeSupportResource CenterSwitchesS6890 SeriesS6890 SeriesTechnical DocumentsReference GuidesCommand ReferencesH3C S6890 Switch Series Command References(R28xx)-6W10011-Network Management and Monitoring Command Reference
04-PTP commands
04-PTP commands 178.94 KB
PTP commands
display ptp clock
Use display ptp clock to display PTP clock information.
display ptp clock
This command does not display any information if you have not specified a PTP profile (PTP standard) or a PTP mode.
# Display PTP clock information.
<Sysname> display ptp clock
PTP profile         : IEEE 1588 Version 2
PTP mode            : BC
Slave only          : No
Clock ID            : 000FE2-FFFE-FF0000
Clock type          : ToD1
 ToD direction  : In
 ToD delay time : 0 (ns)
Clock type          : ToD1
 ToD direction  : In
Clock domain        : 0
Number of PTP ports : 2
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 65535
Offset from master : -4 (ns)
Mean path delay    : 101 (ns)
Steps removed      : 1
Local clock time   : Sun Jan 15 20:57:29 2011
PTP profile
PTP standard:
·     IEEE 1588 version 2.
·     IEEE 802.1AS.
·     SMPTE ST 2059-2.
PTP mode
Clock node type:
·     BC.
·     E2ETC.
·     E2ETC-OC.
·     OC.
·     P2PTC.
·     P2PTC-OC.
Slave only
Whether the OC operates in Slave only mode:
·     Yes.
·     No.
Clock ID
Clock ID for the device, which uniquely identifies a PTP device.
Clock type
Clock type of the device. The value is Local, indicating a local clock.
Clock domain
PTP domain where the device resides.
Priority1
Priority 1 value for the device.
Priority2
Priority 2 value for the device.
Class
Time class of the device.
Accuracy
Time accuracy of the device.
Offset of the grandmaster clock.
Offset from master
Offset from the master clock node (parent clock node), in nanoseconds.
N/A indicates that information for this field is not obtained.
Mean path delay
Mean path delay, in nanoseconds.
Steps removed
Hops from the grandmaster to the local clock node.
display ptp corrections
Use display ptp corrections to display PTP corrections that have occurred on a subordinate port.
The PTP corrections are displayed only when the following conditions are met:
·     You have specified a PTP profile and PTP mode for the device.
·     The device has a subordinate port and has performed time or frequency synchronization through the port.
If the subordinate port is changed, the recorded information will be cleared.
# Display PTP corrections that have occurred on a subordinate port.
<Sysname> display ptp corrections
Slave port   Correction time          Corrections(s,ns)     Rate ratio
XGE1/0/1     Mar 11 03:14:54 2012     0,74                  0.999999973
XGE1/0/1     Mar 11 03:14:55 2012    -1,17                  0.999999980
Slave port
Name of the subordinate port.
Correction time
Time when the correction occurred.
Corrections(s,ns)
Time corrections in seconds or nanoseconds.
N/A indicates that no correction occurred this time.
Rate ratio
Ratio of the subordinate port rate to the master port rate.
display ptp foreign-masters-record
Use display ptp foreign-masters-record to display information about foreign master nodes.
display ptp foreign-masters-record [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays information about foreign master nodes for all interfaces.
Foreign master node information is displayed only when the following conditions are met:
·     You have specified the IEEE 1588 version 2 or SMPTE ST 2059-2 PTP profile.
·     You have specified a PTP mode for the device.
·     The device has a port in slave, passive, or uncalibrated state.
# Display information about foreign master nodes for all interfaces.
<Sysname> display ptp foreign-masters-record
P1=Priority1, P2=Priority2, C=Class, A=Accuracy,
OSLV=Offset-scaled-log-variance, SR=Steps-removed
GM=Grandmaster
Interface    Clock ID             P1   P2   C    A    OSLV   SR   GM
XGE1/0/1     000FE2-FFFE-FF0000   0    128  248  254  65535  0    Yes
XGE1/0/2     000FE2-FFFE-FF0001   0    128  248  254  65535  1    No
Name of a PTP interface.
Clock ID
Clock ID of the foreign master node.
C
Time class.
A
Time accuracy.
OSLV
SR
GM
Whether the node represents the grandmaster clock:
·     Yes.
·     No.
display ptp interface
Use display ptp interface to display PTP running information for an interface.
display ptp interface [ interface-type interface-number | brief ]
interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays PTP running information for all interfaces.
brief: Displays brief PTP running information for all interfaces. If you do not specify this keyword, this command displays detailed PTP running information for the specified interface or all interfaces.
The detailed PTP running information can be displayed only if you enable PTP on the interface. The brief PTP running information can be displayed only when PTP is operating on the interface.
# Display brief PTP running information for all interfaces.
<Sysname> display ptp interface brief
Name         State        Delay mechanism  Clock step  Asymmetry correction
XGE1/0/1     Slave        E2E              Two         0
XGE1/0/2     Passive      E2E              Two         0
# Display detailed PTP running information for Ten-GigabitEthernet 1/0/1.
<Sysname> display ptp interface ten-gigabitethernet 1/0/1
Port number                 : 15
PTP version                 : 2
PTP enable                  : Enabled
Transport of PTP            : User Datagram Protocol (IPv4)
Unicast destination address : 10.10.10.2
DSCP priority               : 56
Port state                  : Slave
Force state                 : No
Clock step                  : Two
Asymmetry correction        : 0
Delay mechanism             : End to End
Announce interval (log mean)           : 1
Announce receipt time out              : 3
Sync interval (log mean)               : 2
Delay request interval (log mean)      : 2
Peer delay request interval (log mean) : 0
Mean path delay                        : 0 (ns)
Name
Name of the PTP interface.
States of the PTP interface:
·     Slave—Receives synchronization messages.
·     Uncalibrated—Temporary state before the interface enters Slave state.
·     Passive—Neither receives nor sends synchronization messages. A PTP interface is in passive state after it receives an announce messages.
·     Master—Sends synchronization messages.
·     Premaster—Temporary state before the interface enters Master state.
·     Listening—Neither receives nor sends synchronization messages. A PTP interface is in listening state after being initialized.
·     Faulty—PTP is running incorrectly. A PTP interface in faulty state does not process PTP messages.
·     Disabled—PTP is not running on the interface. A PTP interface in disabled state does not process PTP messages.
·     Initializing—The interface is initializing. A PTP interface in initializing state does not process PTP messages.
·     N/A—No PTP interface state is obtained.
Delay mechanism
Delay measurement mechanism:
·     End to End—Request-response mechanism.
·     Peer to Peer—Peer delay mechanism.
Clock step
Mode for carrying timestamps:
·     One—Single-step mode. This field is not supported in the current software version.
·     Two—Two-step mode.
Asymmetric delay correction value (in nanoseconds).
Clock ID
Clock ID of the device where the interface resides.
PTP version
PTP version number. The version number is always 2.
PTP enable
Whether PTP is enabled or disabled:
·     Enabled.
·     Disabled.
Transport of PTP
PTP message transport protocol:
·     User Datagram Protocol (IPv4).
·     IEEE 802.3/Ethernet.
Destination IP address for unicast PTP messages that are transmitted over IPv4 UDP. This field is not displayed if the ptp unicast-destination command is not executed.
DSCP priority
DSCP value for PTP messages that are transmitted over IPv4 UDP. This field is not displayed if the ptp dscp command is not executed.
VLAN
VLAN ID for PTP messages. This field is not displayed if the ptp vlan command is not executed.
Dot1p priority
802.1p precedence for PTP messages. This field is not displayed if the ptp vlan command is not executed.
Force state
Whether the force state is configured:
·     Yes.
·     No.
Announce message sending interval (in seconds) = 2interna. This field displays the value for the interval exponent.
Number of announcement intervals before the receiving node stops receiving announce messages. If a member node does not receive any announce message from the master node within the specified value, it considers the master node invalid.
Sync message sending interval (in seconds) = 2interval. This field displays the value for the interval exponent.
Minimum delay request message sending interval (in seconds) = 2interval. This field displays the value for the interval exponent.
Peer delay request message sending interval (in seconds) = 2interval. This field displays the value for the interval exponent.
Mean path delay
display ptp parent
Use display ptp parent to display parent node (master node) information for the PTP device.
display ptp parent
The command does not display any information in any of the following circumstances:
·     You have not specified a PTP profile or a PTP mode for the device.
·     You have specified the TC clock node type.
·     You have executed the ptp active force-state command.
# Display parent node information for the PTP device.
<Sysname> display ptp parent
Parent clock:
 Parent clock ID                         : 000FE2-FFFE-FF0005
 Parent port number                      : 15
 Observed parent offset (log variance)   : N/A
 Observed parent clock phase change rate : N/A
Grandmaster clock:
 Grandmaster clock ID: 000FE2-FFFE-FF0000
 Grandmaster clock quality:
  Class                 : 248
  Accuracy              : 254
  Priority1             : 128
  Priority2             : 128
Table 5 Command output
Parent port number
Outgoing interface number of the parent clock.
Offset from the parent clock node.
Class
Time class of the grandmaster clock.
Accuracy
Time accuracy of the grandmaster clock.
Priority1
Priority 1 value of the grandmaster clock.
Priority2
Priority 2 value of the grandmaster clock.
display ptp statistics
Use display ptp statistics to display PTP statistics.
display ptp statistics [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays PTP statistics for all interfaces.
The command does not display any PTP statistics if you have not specified a PTP profile or a PTP mode.
# Display PTP statistics on Ten-GigabitEthernet 1/0/1.
<Sysname> display ptp statistics interface ten-gigabitethernet 1/0/1
                     Received packets
Announce :0          Sync      :0          Signaling          :0
DelayReq :0          DelayResp :0          FollowUp           :0
PdelayReq:0          PdelayResp:0          PdelayRespFollowUp :0
                     Sent packets
Announce :476        Sync      :2543       Signaling          :0
DelayReq :0          DelayResp :0          FollowUp           :2542
PdelayReq:238        PdelayResp:0          PdelayRespFollowUp :0
                     Discarded packets
Table 6 Command output
Received packets
Statistics about received PTP messages.
Sent packets
Statistics about sent PTP messages.
Discarded packets
Statistics about discarded PTP messages.
display ptp time-property
Use display ptp time-property to display PTP clock properties.
This command does not display any information in any of the following circumstances:
·     You have not specified a PTP profile or a clock node type.
·     You have specified the e2etc or p2ptc clock node type.
# Display PTP clock properties.
<Sysname> display ptp time-property
PTP clock time property:
 Current UTC offset valid : True
 Current UTC offset       : 33
 Leap59 : Yes
 Leap61 : No
 Time traceable      : True
 Frequency traceable : True
 PTP timescale       : True
 Time source         : 0xA0 (Internal oscillator)
Table 7 Command output
Whether the Coordinated Universal Time (UTC) offset is valid:
·     True—Yes.
·     False—No.
Current UTC offset
Cumulative offset (in seconds) between the UTC of the grandmaster clock and the International Atomic Time (TAI).
Leap59
Whether cumulative offset is minus 1:
·     Yes.
·     No.
Leap61
Whether cumulative offset is plus 1:
·     Yes.
·     No.
Time traceable
Whether the PTP time is traceable:
·     True—Yes.
·     False—No.
Frequency traceable
Whether the PTP frequency is traceable:
·     True—Yes.
·     False—No.
PTP timescale
The possible timescales available for use by the grandmaster clock:
·     True—PTP timescale.
·     False—Non-PTP timescale.
Time source
Attributes of the grandmaster clock:
·     Atomic clock.
·     GPS.
·     Handset.
·     Internal oscillator.
·     NTP.
·     Other.
·     PTP.
·     Terrestrial radio.
·     Unknown.
Use ptp active force-state to activate the port role configuration.
Use undo ptp active force-state to restore the default.
The port role configuration is not activated.
This command is available only after you specify a PTP profile and a PTP mode.
# Activate the port role configuration.
[Sysname] ptp profile 1588v2
[Sysname] ptp mode oc
[Sysname] ptp active force-state
ptp force-state
ptp mode
ptp profile
ptp announce-interval
Use ptp announce-interval to set the interval for sending announce messages.
Use undo ptp announce-interval to restore the default.
ptp announce-interval interval
For the IEEE 1588 version 2 PTP profile, the interval argument value is 1 and the announce message sending interval is 2 (21) seconds.
For the IEEE 802.1AS PTP profile, the interval argument value is 0 and the announce message sending interval is 1 (20) second.
For the SMPTE ST 2059-2 PTP profile, the interval argument value is –2 and the announce message sending interval is 1/4 (2-2) second.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending announce messages. When the PTP profile is IEEE 1588 version 2, the value range for the interval argument is 0 to 4. When the PTP profile is IEEE 802.1AS, the value range for the interval argument is 0 to 6. When the PTP profile is SMPTE ST 2059-2, the value range for the interval argument is –3 to 1.
The master node uses the value configured on its interface as the interval for sending announce messages.
# Set the announce message sending interval to 4 (22) seconds on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp announce-interval 2
ptp mode
ptp profile
ptp announce-timeout
Use ptp announce-timeout to set the timeout multiplier for the announce message receiving interval.
Use undo ptp announce-timeout to restore the default.
ptp announce-timeout multiple-value
The timeout multiplier for the announce message receiving interval is 3.
multiple-value: Sets the timeout multiplier for the announce message receiving interval, in the range of 2 to 10.
A master node periodically sends announce messages to the member nodes.
·     IEEE 1588 version 2 or SMPTE ST 2059-2—If a member node does not receive any announce message from the master node within multiple-value times the announce message sending interval, it determines that the master node is invalid.
·     IEEE 802.1AS—If a member node does not receive any announce message from the master node within multiple-value times the announce message sending interval configured on the master node, it determines that the master node is invalid.
To ensure a stable PTP network, set the timeout multiplier for receiving announce messages to a value in the range of 5 to 7.
# Set the timeout multiplier for the announce message sending interval to 5 on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp announce-timeout 5
ptp mode
ptp profile
ptp asymmetry-correction
Use ptp asymmetry-correction to set the asymmetric delay correction time.
Use undo ptp asymmetry-correction to restore the default.
ptp asymmetry-correction { minus | plus } value
The asymmetric delay correction time is 0 nanoseconds, which means that delay correction is not performed.
minus: Subtracts the specified asymmetric delay correction value.
plus: Adds the specified asymmetric delay correction value.
value: Specifies the asymmetric delay correction value in the range of 0 to 2000000 nanoseconds.
# Set the asymmetric delay correction time to 100 nanoseconds on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp asymmetry-correction plus 100
ptp mode
ptp profile
ptp delay-mechanism
Use ptp delay-mechanism to specify a delay measurement mechanism for a BC or an OC.
Use undo ptp delay-mechanism to restore the default.
ptp delay-mechanism { e2e | p2p }
The default setting varies by PTP profile:
·     IEEE 1588 version 2 or SMPTE ST 2059-2 PTP profile—The request-response delay measurement applies.
·     IEEE 802.1AS PTP profile—The peer delay measurement mechanism applies.
e2e: Specifies the request-response mechanism.
p2p: Specifies the peer delay mechanism.
You can configure this command only after you have specified a PTP profile and PTP mode for the device. Follow these restrictions and guidelines when you configure this command:
·     IEEE 1588 version 2 or SMPTE ST 2059-2 PTP profile:
¡     You can configure this command only for a BC or OC clock node.
¡     The E2ETC, E2ETC+OC, P2PTC, and P2PTC+OC clock nodes do not support this command. The E2ETC and E2ETC+OC clock nodes support both the request-response and peer delay measurement mechanisms. The P2PTC clock node supports only the peer delay measurement mechanism.
·     IEEE 802.1AS PTP profile: Supports only the peer delay measurement mechanism and does not support this command.
# Specify the OC clock node type. Specify the request-response delay measurement mechanism (e2e) on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp delay-mechanism e2e
ptp mode
ptp profile
ptp destination-mac
Use ptp destination-mac to configure the destination MAC address for non-peer delay messages.
Use undo ptp destination-mac to restore the default.
ptp destination-mac mac-address
The destination MAC address for non-peer delay messages is 011B-1900-0000.
mac-address: Specifies the destination MAC address for non-peer delay messages as 0180-C200-000E or 011B-1900-0000.
This command is available only after you specify IEEE 1588 version 2 or SMPTE ST 2059-2 as the PTP profile and specify a PTP mode.
Peer delay messages include Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages. The destination MAC address for peer delay messages is 0180-C200-000E, which cannot be modified.
This command takes effect only if PTP messages are encapsulated in IEEE 802.3/Ethernet packets.
# Configure the destination MAC address for non-peer delay messages as 0180-C200-000E on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp destination-mac 0180-c200-000e
ptp mode
ptp profile
ptp domain
Use ptp domain to specify a PTP domain.
Use undo ptp domain to restore the default.
ptp domain domain-number
undo ptp domain
When the PTP profile is IEEE 1588 version 2 or IEEE 802.1AS, the device is in PTP domain 0.
When the PTP profile is SMPTE ST 2059-2, the device is in PTP domain 127.
domain-number: Specifies a PTP domain by its number. When the PTP profile is IEEE 1588 version 2 or IEEE 802.1AS, the value range for the domain-number argument is 0 to 255. When the PTP profile is SMPTE ST 2059-2, the value range for the domain-number argument is 0 to 127.
# Configure the PTP domain number to use for the device as 2.
[Sysname] ptp domain 2
ptp mode
ptp profile
ptp dscp
Use ptp dscp to set a DSCP value for PTP messages that are transmitted over IPv4 UDP.
Use undo ptp dscp to restore the default.
ptp dscp dscp
undo ptp dscp
The DSCP value is 56 for PTP messages that are transmitted over IPv4 UDP.
dscp: Sets a DSCP value in the range of 0 to 63 for PTP messages.
The IEEE 802.1AS PTP profile does not support this command.
This command takes effect only if PTP messages are transmitted over IPv4 UDP.
# Set the DSCP value to 63 for PTP messages transmitted over IPv4 UDP on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp transport-protocol udp
[Sysname-Ten-GigabitEthernet1/0/1] ptp dscp 63
ptp mode
ptp profile
ptp enable
Use ptp enable to enable PTP.
Use undo ptp enable to disable PTP.
ptp enable
undo ptp enable
PTP is disabled.
You can enable PTP on only one port if the clock node type of the device is OC.
As a best practice, enable PTP on an interface after you configure PTP parameters.
To enable PTP on a Layer 3 Ethernet interface that has been assigned to a VPN instance, you must specify this VPN instance in the ptp source ip-address vpn-instance vpn-instance-name command if PTP messages are to be transmitted in multicast mode over IPv4 UDP.
# Configure the clock node type as OC, and enable PTP on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp enable
# Configure the clock node type as E2ETC, and enable PTP on Ten-GigabitEthernet 1/0/1 and Ten-GigabitEthernet 1/0/2.
[Sysname] ptp mode e2etc
[Sysname-Ten-GigabitEthernet1/0/1] interface ten-gigabitethernet 1/0/2
[Sysname-Ten-GigabitEthernet1/0/2] ptp enable
ptp mode
ptp profile
ptp source
ptp force-state
Use ptp force-state to configure a role for a PTP port.
Use undo ptp force-state to restore the default.
ptp force-state { master | passive | slave }
The PTP port role is automatically calculated by BMC.
master: Specifies the PTP port as a master port.
passive: Specifies the PTP port as a passive port.
slave: Specifies the PTP port as a subordinate port.
By default, the PTP port roles are automatically negotiated based on the BMC algorithm. If you use this command to change the role of one PTP port, all the other PTP ports in the PTP domain stop working. For these PTP ports to function, you must specify roles for each of them by using this command. As a best practice, enable automatic negotiation of PTP port roles based on the BMC algorithm.
You can configure only one subordinate port for a device.
# Configure the clock node type as OC. Specify the PTP port Ten-GigabitEthernet 1/0/1 as a subordinate port.
[Sysname-Ten-GigabitEthernet1/0/1] ptp force-state slave
ptp mode
ptp profile
ptp slave-only
ptp min-delayreq-interval
Use ptp min-delayreq-interval to set the minimum interval for sending delay request messages.
Use undo ptp min-delayreq-interval to restore the default.
ptp min-delayreq-interval interval
When the PTP profile is IEEE 1588 version 2 or SMPTE ST 2059-2, the minimum interval for sending delay request messages is 1 (20) second.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending delay request messages. When the PTP profile is IEEE 1588 version 2, the value range for the interval argument is –4 to 6. When the PTP profile is SMPTE ST 2059-2, the value range for the interval argument is –5 to 4.
When a member clock receives a Sync message, it responds by sending a Delay_Req message and starts a timer defined by this command. The member clock will not send another Delay_Req message until it receives a Sync message after the timer expires.
In PTP multicast transport mode, this command takes effect only when configured on the master clock. The master clock sends the value to a member clock through PTP messages to control the interval for the member clock to send Delay_Req messages. To view the interval, execute the display ptp interface command on the member clock.
In PTP unicast transport mode, this command takes effect when configured on member clocks. It does not take effect when configured on the master clock.
When the PTP profile is SMPTE ST 2059-2, set the interval argument to a value in the range of ptp syn-interval interval to ptp syn-interval interval plus 5 as a best practice.
# Set the minimum interval to 4 (22) seconds for sending delay request messages on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp min-delayreq-interval 2
ptp mode
ptp profile
ptp syn-interval
ptp mode
Use ptp mode to specify a clock node type for the device.
Use undo ptp mode to restore the default.
IEEE 1588v2 PTP profile:
ptp mode { bc | e2etc | e2etc-oc | oc | p2ptc | p2ptc-oc }
undo ptp mode
ptp mode { bc | oc | p2ptc | p2ptc-oc }
undo ptp mode
ptp mode { bc | e2etc | oc | p2ptc }
undo ptp mode
No clock node type is specified.
bc: Specifies the boundary clock (BC) type.
e2etc: Specifies the end-to-end transparent clock (E2ETC) type.
e2etc-oc: Specifies the E2ETC+OC type.
oc: Specifies the ordinary clock (OC) type.
p2ptc: Specifies the peer-to-peer transparent clock (P2PTC) type.
p2ptc-oc: Specifies the P2PTC+OC type.
CAUTION
CAUTION:
If you change the clock node type for the device, all settings except for the PTP profile will be removed.
This command is available only after you specify a PTP profile.
When the PTP profile is IEEE 802.1AS, you cannot specify the E2ETC or E2ETC+OC clock node type.
When the PTP profile is SMPTE ST 2059-2, you cannot specify the E2ETC+OC or P2PTC+OC clock node type.
# Specify the OC clock node type for the device.
ptp profile
ptp pdelay-req-interval
Use ptp pdelay-req-interval to set the interval for sending peer delay request messages.
Use undo ptp pdelay-req-interval to restore the default.
ptp pdelay-req-interval interval
The interval for sending peer delay request messages is 1 (20) second.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending peer delay request messages. When the PTP profile is IEEE 1588 version 2, the value range for the interval argument is 0 to 5. When the PTP profile is IEEE 802.1AS, the value range for the interval argument is –4 to 6. When the PTP profile is SMPTE ST 2059-2, the value range for the interval argument is –5 to 4.
# Set the interval to 4 (22) seconds for sending peer delay request messages on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp pdelay-req-interval 2
ptp mode
ptp profile
ptp syn-interval
ptp port-mode
Use ptp port-mode to configure the port type as OC for a TC+OC (including E2ETC+OC and P2PTC+OC) clock.
Use undo ptp port-mode to restore the default.
ptp port-mode oc
undo ptp port-mode
The type of all ports on an E2ETC+OC or a P2PTC+OC clock is TC.
oc: Specifies the port type for a TC+OC clock as OC.
This command is applicable only to E2ETC+OC and P2PTC+OC clocks and is available only after you specify a PTP profile and a PTP mode.
The SMPTE ST 2059-2 PTP profile does not support this command.
# Specify the P2PTC+OC clock node type for the device. Specify the OC port type for Ten-GigabitEthernet 1/0/1.
[Sysname] ptp mode p2ptc-oc
[Sysname-Ten-GigabitEthernet1/0/1] ptp port-mode oc
ptp mode
ptp profile
ptp priority
Use ptp priority clock-source to configure the priority for the specified clock for GM election through BMC.
Use undo ptp priority clock-source to restore the specified priority to its default value.
ptp priority clock-source local { priority1 priority1 | priority2 priority2 }
undo ptp priority clock-source local { priority1 | priority2 }
When the PTP profile is IEEE 1588 version 2 or SMPTE ST 2059-2, the priority 1 and priority 2 values are both 128.
When the PTP profile is IEEE 802.1AS, the priority 1 value is 246 and the priority 2 value is 248.
local: Specifies the local clock.
priority1 priority1: Specifies priority 1 for the clock, in the range of 0 to 255. A numerically smaller value has higher priority.
priority2 priority2: Specifies priority 2 for the clock, in the range of 0 to 255. A numerically smaller value has higher priority.
# Set priority 1 to 10 for the local clock.
[Sysname] ptp priority clock-source local priority1 10
ptp mode
ptp profile
ptp profile
Use ptp profile to specify a PTP profile for the device.
Use undo ptp profile to restore the default.
ptp profile { 1588v2 | 8021as | st2059-2 }
undo ptp profile
PTP operates only after you specify a PTP profile.
1588v2: Specifies the IEEE 1588 version 2 PTP profile.
8021as: Specifies the IEEE 802.1AS PTP profile.
st2059-2: Specifies the SMPTE ST 2059-2 PTP profile.
Specify a PTP profile for the device before any other PTP configurations.
Changing or removing a PTP profile clears all settings under the PTP profile.
# Specify the IEEE 1588 version 2 PTP profile.
ptp slave-only
Use ptp slave-only to configure the OC to operate only as a member clock.
Use undo ptp slave-only to restore the default.
ptp slave-only
undo ptp slave-only
An OC can operate either as a master clock or a member clock.
This command is applicable only to OCs and is available only after you specify a PTP profile and a PTP mode.
You can execute the ptp force-state command to specify a subordinate port as a master port or passive port even if the OC operates as a member clock.
# Specify the OC clock node type for the device. Configure the OC to operate only as a member clock.
[Sysname] ptp slave-only
ptp force-state
ptp mode
ptp profile
ptp source
Use ptp source to configure the source IP address for multicast PTP messages transmitted over IPv4 UDP.
Use undo ptp source to remove the specified source IP address for multicast PTP messages transmitted over IPv4 UDP.
ptp source ip-address [ vpn-instance vpn-instance-name ]
undo ptp source ip-address [ vpn-instance vpn-instance-name ]
No source IP address is configured for multicast PTP messages transmitted over IPv4 UDP.
ip-address: Specifies the source IP address for multicast PTP messages transmitted over IPv4 UDP.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance used for communication between the local device and the peer device. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If the peer device belongs to the public network, do not specify this option.
This command is available only after you specify a PTP profile and a PTP mode. The IEEE 802.1AS profile does not support this command.
This command takes effect only when PTP messages are transmitted over IPv4 UDP in multicast mode.
If a PTP-enabled Layer 3 Ethernet interface has been assigned to a VPN instance, you must specify the VPN instance in the ptp source ip-address vpn-instance vpn-instance-name command.
# Configure the source IP address as 3.5.1.5 for multicast PTP messages transmitted over IPv4 UDP.
[Sysname] ptp source 3.5.1.5
ptp mode
ptp profile
ptp syn-interval
Use ptp syn-interval to set the interval for sending Sync messages.
Use undo ptp syn-interval to restore the default.
When the PTP profile is IEEE 1588 version 2, the interval argument value is 0 and the interval for sending Sync messages is 1 (20) second.
When the PTP profile is IEEE 802.1AS or SMPTE ST 2059-2, the interval argument value is –3 and the interval for sending Sync messages is 1/8 (2-3) seconds.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending Sync messages. When the PTP profile is IEEE 802.1AS, the value range for the interval argument is -4 to 6. When the PTP profile is IEEE 1588 version 2, the value range for the interval argument is -1 to 1. When the PTP profile is SMPTE ST 2059-2, the value range for the interval argument is –5 to –1.
# Set the Sync message sending interval to 2 (21) seconds on Ten-GigabitEthernet 1/0/1.
[Sysname-Ten-GigabitEthernet1/0/1] ptp syn-interval 1
ptp mode
ptp profile
Use ptp transport-protocol to configure the IPv4 UDP transport protocol for PTP messages.
Use undo ptp transport-protocol to restore the default.
PTP messages are transported through IEEE 802.3 and Ethernet.
udp: Specifies the IPv4 UDP transport protocol for PTP messages.
This command is not available for the IEEE 802.1AS or SMPTE ST 2059-2 PTP profile.
# Configure the IPv4 UDP transport protocol for PTP messages on Ten-GigabitEthernet 1/0/1.
ptp mode
ptp profile
Use ptp unicast-destination to configure the destination IP address for unicast PTP messages transmitted over IPv4 UDP.
Use undo ptp unicast-destination to restore the default.
ptp unicast-destination ip-address
undo ptp unicast-destination ip-address
No destination IP address is configured for unicast PTP messages transmitted over IPv4 UDP.
ip-address: Specifies the destination IP address for unicast PTP messages transmitted over IPv4 UDP.
This command takes effect only when PTP messages are transmitted over IPv4 UDP.
# Configure the destination IP address as 10.10.10.2 for unicast PTP messages transmitted over IPv4 UDP.
[Sysname-Ten-GigabitEthernet1/0/1] ptp unicast-destination 10.10.10.2
ptp mode
ptp profile
ptp utc
Use ptp utc to add or subtract one second from the UTC scale on the specified date.
Use undo ptp utc to restore the default.
ptp utc { leap59-date | leap61-date } date
undo ptp utc { leap59-date | leap61-date }
No second is added to or subtracted from the UTC scale.
leap59-date: Subtracts one second from the UTC time scale at the last minute (23:59) on the specified date.
leap61-date: Adds one second to the UTC time scale at the last minute (23:59) on the specified date.
date: Sets the date to adjust UTC, in the format of YYYY/MM/DD. The value range for YYYY and MM is 2000 to 2035 and 1 to 12, respectively. The value range for DD depends on the specified month. For the configuration to take effect, do not specify a date earlier than the current date.
UTC is based on International Atomic Time (TAI), a high-precision atomic coordinate time scale, and adjusted by leap seconds for synchronization with astronomical time.
UTC is constantly compared with UT1 (astronomical time, reflecting the earth's rotation). The International Bureau of Weights and Measures (BIPM) will notify to add or subtract one second from the UTC time scale at the last minute on a specific date (typically June 30 or December 31) to ensure that the difference between UTC and UT1 is within one second.
You can use this command to add or subtract one second from the UTC time on the specific date as published by BIPM.
This command takes effect only when it is configured on the master clock node and the local clock of the master clock node is the GM.
# Assume that the current date is August 8, 2016. Specify the BC clock node type for the device. According to information published by BIPM, add one second to the UTC time at 23:59:60 on December 31, 2016.
[Sysname] ptp mode bc
[Sysname] ptp utc offset 36
[Sysname] ptp utc leap61-date 2016/12/31
ptp mode
ptp profile
ptp utc offset
ptp utc offset
Use ptp utc offset to set the cumulative offset of UTC relative to TAI.
Use undo ptp utc offset to restore the default.
ptp utc offset utc-offset
undo ptp utc offset
The cumulative offset of UTC relative to TAI is 0 seconds.
utc-offset: Sets the cumulative offset of UTC relative to TAI, in seconds. The value range for the utc-offset argument is 0 to 999.
A time difference exists between UTC and TAI. Internet devices typically use the UTC time. To provide more accurate time, PTP also uses TAI. If the device acts as a subordinate clock node, it uses the UTC time and TAI time of the clock reference. If the device acts as the clock reference, it will calculate the TAI time based on the UTC time and synchronize the UTC and TAI time to the subordinate clocks. TAI provided by the device = Current UTC + cumulative offset + leap second.
BIPM periodically publishes the cumulative offset of UTC relative to TAI. Use the value published by BIPM to configure this command.
# According to information published by BIPM, the cumulative offset of UTC relative to TAI is 37 seconds. Set the cumulative offset of UTC relative to TAI to 37 seconds.
[Sysname] ptp utc offset 37
ptp mode
ptp profile
ptp utc
ptp vlan
Use ptp vlan to specify a VLAN tag for PTP messages.
Use undo ptp vlan to restore the default.
ptp vlan vlan-id [ dot1p dot1p-value ]
undo ptp vlan [ dot1p ]
PTP messages do not have a VLAN tag.
vlan vlan-id: Specifies a VLAN by its ID. The value range for the vlan-id argument is 1 to 4094.
dot1p dot1p-value: Specifies an 802.1p precedence for PTP messages, in the range of 0 to 7. The default 802.1p precedence is 7 (the highest).
# Specify VLAN 2 and set the 802.1p precedence to 6 for PTP messages.
[Sysname-Ten-GigabitEthernet1/0/1] ptp vlan 2 dot1p 6
ptp mode
ptp profile
reset ptp statistics
Use reset ptp statistics to clear PTP statistics.
reset ptp statistics [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command clears PTP statistics on all interfaces.
# Clear PTP statistics on Ten-GigabitEthernet 1/0/1.
<Sysname> reset ptp statistics interface ten-gigabitethernet 1/0/1
  • Become a Partner
  • Partner Resources
