17-Network Management and Monitoring Configuration Guide
HomeSupportConfigure & DeployConfiguration GuidesH3C SecPath M9000 Configuration Guide(V7)(R9153P39 R9001P39)-6W40017-Network Management and Monitoring Configuration Guide
12-Event MIB configuration
12-Event MIB configuration 116.65 KB
Configuring the Event MIB
About the Event MIB
The Event Management Information Base (Event MIB) is an SNMPv3-based network management protocol and is an enhancement to remote network monitoring (RMON). The Event MIB uses Boolean tests, existence tests, and threshold tests to monitor MIB objects on a local or remote system. It triggers the predefined notification or set action when a monitored object meets the trigger condition.
Trigger
The Event MIB uses triggers to manage and associate the three elements of the Event MIB: monitored object, trigger condition, and action.
Monitored objects
The Event MIB can monitor the following MIB objects:
·     Table node.
·     Conceptual row node.
·     Table column node.
·     Simple leaf node.
·     Parent node of a leaf node.
To monitor a single MIB object, specify it by its OID or name. To monitor a set of MIB objects, specify the common OID or name of the group and enable wildcard matching. For example, specify ifDescr.2 to monitor the description for the interface with index 2. Specify ifDescr and enable wildcard matching to monitor the descriptions for all interfaces.
Trigger test
A trigger supports Boolean, existence, and threshold tests.
Boolean test
A Boolean test compares the value of the monitored object with the reference value and takes actions according to the comparison result. The comparison types include unequal, equal, less, lessorequal, greater, and greaterorequal. For example, if the comparison type is equal, an event is triggered when the value of the monitored object equals the reference value. The event will not be triggered again until the value becomes unequal and comes back to equal.
Existence test
An existence test monitors and manages the absence, presence, and change of a MIB object, for example, interface status. When a monitored object is specified, the system reads the value of the monitored object regularly.
·     If the test type is Absent, the system triggers an alarm event and takes the specified action when the state of the monitored object changes to absent.
·     If the test type is Present, the system triggers an alarm event and takes the specified action when the state of the monitored object changes to present.
·     If the test type is Changed, the system triggers an alarm event and takes the specified action when the value of the monitored object changes.
Threshold test
A threshold test regularly compares the value of the monitored object with the threshold values.
·     A rising alarm event is triggered if the value of the monitored object is greater than or equal to the rising threshold.
·     A falling alarm event is triggered if the value of the monitored object is smaller than or equal to the falling threshold.
·     A rising alarm event is triggered if the difference between the current sampled value and the previous sampled value is greater than or equal to the delta rising threshold.
·     A falling alarm event is triggered if the difference between the current sampled value and the previous sampled value is smaller than or equal to the delta falling threshold.
·     A falling alarm event is triggered if the values of the monitored object, the rising threshold, and the falling threshold are the same.
·     A falling alarm event is triggered if the delta rising threshold, the delta falling threshold, and the difference between the current sampled value and the previous sampled value is the same.
The alarm management module defines the set or notification action to take on alarm events.
If the value of the monitored object crosses a threshold multiple times in succession, the managed device triggers an alarm event only for the first crossing. For example, if the value of a sampled object crosses the rising threshold multiple times before it crosses the falling threshold, only the first crossing triggers a rising alarm event, as shown in Figure 1.
Figure 1 Rising and falling alarm events
Event actions
The Event MIB triggers one or both of the following actions when the trigger condition is met:
·     Set action—Uses SNMP to set the value of the monitored object.
·     Notification action—Uses SNMP to send a notification to the NMS. If an object list is specified for the notification action, the notification will carry the specified objects in the object list.
Object list
An object list is a set of MIB objects. You can specify an object list in trigger view, trigger-test view (including trigger-Boolean view, trigger existence view, and trigger threshold view), and action-notification view. If a notification action is triggered, the device sends a notification carrying the object list to the NMS.
If you specify an object list respectively in any two of the views or all the three views, the object lists are added to the triggered notifications in this sequence: trigger view, trigger-test view, and action-notification view.
Object owner
Trigger, event, and object list use an owner and name for unique identification. The owner must be an SNMPv3 user that has been created on the device. If you specify a notification action for a trigger, you must establish an SNMPv3 connection between the device and NMS by using the SNMPv3 username. For more information about SNMPv3 user, see "SNMP configuration".
Restrictions and guidelines: Event MIB configuration
The Event MIB and RMON are independent of each other. You can configure one or both of the features for network management.
You must specify the same owner for a trigger, object lists of the trigger, and events of the trigger.
Event MIB tasks at a glance
To configure the Event MIB, perform the following tasks:
1.     Configuring the Event MIB global sampling parameters
2.     (Optional.) Configuring Event MIB object lists
Perform this task so that the device sends a notification that carries the specified object list to the NMS when a notification action is triggered.
3.     Configuring an event
The device supports set and notification actions. Choose one or two of the following actions:
¡     Creating an event
¡     Configuring a set action for an event
¡     Configuring a notification action for an event
¡     Enabling the event
4.     Configuring a trigger
A trigger supports Boolean, existence, and threshold tests. Choose one or more of the following tests:
¡     Creating a trigger and configuring its basic parameters
¡     Configuring a Boolean trigger test
¡     Configuring an existence trigger test
¡     Configuring a threshold trigger test
¡     Enabling trigger sampling
5.     (Optional.) Enabling SNMP notifications for the Event MIB module
Prerequisites for configuring the Event MIB
Before you configure the Event MIB, perform the following tasks:
·     Create an SNMPv3 user. Assign the user the rights to read and set the values of the specified MIB objects and object lists.
·     Make sure the SNMP agent and NMS are configured correctly and the SNMP agent can send notifications to the NMS correctly.
This tasks takes effect only on monitored instances to be created.
2.     Set the minimum sampling interval.
snmp mib event sample minimum min-number
By default, the minimum sampling interval is 1 second.
The sampling interval of a trigger must be greater than the minimum sampling interval.
3.     Configure the maximum number of object instances that can be concurrently sampled.
snmp mib event sample instance maximum max-number
By default, the value is 0. The maximum number of object instances that can be concurrently sampled is limited by the available resources.
Perform this task so that the device sends a notification that carries the specified objects to the NMS when a notification action is triggered.
2.     Configure an Event MIB object list.
snmp mib event object list owner group-owner name group-name object-index oid object-identifier [ wildcard ]
The object can be a table node, conceptual row node, table column node, simple leaf node, or parent node of a leaf node.
Creating an event
2.     Create an event and enter its view.
snmp mib event owner event-owner name event-name
3.     (Optional.) Configure a description for the event.
By default, an event does not have a description.
2.     Enter event view.
3.     Enable the set action and enter set action view.
action set
By default, no action is specified for an event.
4.     Specify an object by its OID for the set action.
By default, no object is specified for a set action.
5.     Enable OID wildcarding.
wildcard oid
By default, OID wildcarding is disabled.
6.     Set the value for the object.
value integer-value
The default value for the object is 0.
7.     (Optional.) Specify a context for the object.
context context-name
By default, no context is specified for an object.
8.     (Optional.) Enable context wildcarding.
wildcard context
By default, context wildcarding is disabled.
A wildcard context contains the specified context and the wildcarded part.
2.     Enter event view
3.     Enable the notification action and enter notification action view.
action notification
4.     Specify an object to execute the notification action by its OID.
By default, no object is specified for executing the notification action.
The object must be a notification object.
5.     Specify an object list to be added to the notification triggered by the event.
By default, no object list is specified for the notification action.
If you do not specify an object list for the notification action or the specified object list does not contain variables, no variables will be carried in the notification.
Enabling the event
The Boolean, existence, and threshold events can be triggered only after you perform this task.
To change an enabled event, first disable the event.
3.     Enable the event.
event enable
By default, an event is disabled.
2.     Create a trigger and enter its view.
snmp mib event trigger owner trigger-owner name trigger-name
The trigger owner must be an existing SNMPv3 user.
3.     (Optional.) Configure a description for the trigger.
By default, a trigger does not have a description.
4.     Set a sampling interval for the trigger.
frequency interval
By default, the sampling interval is 600 seconds.
Make sure the sampling interval is greater than or equal to the Event MIB minimum sampling interval.
5.     Specify a sampling method.
sample { absolute | delta }
The default sampling method is absolute.
6.     Specify an object to be sampled by its OID.
By default, the OID is 0.0. No object is specified for a trigger.
7.     (Optional.) Enable OID wildcarding.
wildcard oid
8.     (Optional.) Configure a context for the monitored object.
By default, no context is configured for a monitored object.
9.     (Optional.) Enable context wildcarding.
wildcard context
10.     (Optional.) Specify the object list to be added to the triggered notification.
By default, no object list is specified for a trigger.
2.     Enter trigger view.
3.     Specify a Boolean test for the trigger and enter trigger-Boolean view.
test boolean
By default, no test is configured for a trigger.
4.     Specify a Boolean test comparison type.
comparison { equal | greater | greaterorequal | less | lessorequal | unequal }
The default Boolean test comparison type is unequal.
5.     Set a reference value for the Boolean trigger test.
value integer-value
The default reference value for a Boolean trigger test is 0.
6.     Specify an event for the Boolean trigger test.
By default, no event is specified for a Boolean trigger test.
7.     (Optional.) Specify the object list to be added to the notification triggered by the test.
By default, no object list is specified for a Boolean trigger test.
8.     Enable the event to be triggered when the trigger condition is met at the first sampling.
startup enable
By default, the event is triggered when the trigger condition is met at the first sampling.
Before the first sampling, you must enable this command to allow the event to be triggered.
3.     Specify an existence test for the trigger and enter trigger-existence view.
test existence
By default ,no test is configured for a trigger.
4.     Specify an event for the existence trigger test.
By default, no event is specified for an existence trigger test.
5.     (Optional.) Specify the object list to be added to the notification triggered by the test.
By default, no object list is specified for an existence trigger test.
6.     Specify an existence trigger test type.
type { absent | changed | present }
The default existence trigger test types are present and absent.
7.     Specify an existence trigger test type for the first sampling.
startup { absent | present }
By default, both the present and absent existence trigger test types are allowed for the first sampling.
3.     Specify a threshold test for the trigger and enter trigger-threshold view.
test boolean
4.     Specify the object list to be added to the notification triggered by the test.
By default, no object list is specified for a threshold trigger test.
5.     (Optional.) Specify the type of the threshold trigger test for the first sampling.
startup { falling | rising | rising-or-falling }
The default threshold trigger test type for the first sampling is rising-or-falling.
6.     Specify the delta falling threshold and the falling alarm event triggered when the delta value (difference between the current sampled value and the previous sampled value) is smaller than or equal to the delta falling threshold.
delta falling { event owner event-owner name event-name | value integer-value }
By default, the delta falling threshold is 0, and no falling alarm event is specified.
7.     Specify the delta rising threshold and the rising alarm event triggered when the delta value is greater than or equal to the delta rising threshold.
delta rising { event owner event-owner name event-name | value integer-value }
By default, the delta rising threshold is 0, and no rising alarm event is specified.
8.     Specify the falling threshold and the falling alarm event triggered when the sampled value is smaller than or equal to the threshold.
By default, the falling threshold is 0, and no falling alarm event is specified.
9.     Specify the rising threshold and the ring alarm event triggered when the sampled value is greater than or equal to the threshold.
By default, the rising threshold is 0, and no rising alarm event is specified.
Enable trigger sampling after you complete trigger parameters configuration. You cannot modify trigger parameters after trigger sampling is enabled. To modify trigger parameters, first disable trigger sampling.
3.     Enable trigger sampling.
trigger enable
By default, trigger sampling is disabled.
To report critical Event MIB events to an NMS, enable SNMP notifications for the Event MIB module. For Event MIB event notifications to be sent correctly, you must also configure SNMP on the device. For more information about SNMP configuration, see the network management and monitoring configuration guide for the device.
2.     Enable snmp notifications for the Event MIB module.
snmp-agent trap enable event-mib
By default, SNMP notifications are enabled for the Event MIB module.
Display and maintenance commands for Event MIB
Display Event MIB configuration and statistics.
display snmp mib event
Display event information.
display snmp mib event event [ owner event-owner name event-name ]
Display object list information.
display snmp mib event object list [ owner group-owner name group-name ]
Display global Event MIB configuration and statistics.
display snmp mib event summary
Display trigger information.
display snmp mib event trigger [ owner trigger-owner name trigger-name ]