| 01-Hardware Information and Specifications | 3.07 MB |
1 Product models and technical specifications
Removable components available for the switch
PSR1600C-12A-B AC power supply
PSR1300-12A-C-A AC power supply
PSR1300-12A-C-B AC power supply
PSR2400B-12D-B DC power supply
Product models
The H3C S9825 & S9855 switch series include the following models:
Series |
Product model |
Product code |
H3C S9825 and S9855 switch series |
S9825-64D |
· LS-9825-64D · LS-9825-64D-H1 |
S9855-32D |
LS-9855-32D |
S9855-48CD8D |
LS-9855-48CD8D |
S9855-24B8D |
LS-9855-24B8D |
S9855-40B |
LS-9855-40B |
H3C S9825 and S9855 switch series are a new generation of high-performance and high-density 400GE, 200GE, and 100GE switches launched by H3C for data centers and high-end campuses. The S9825 and S9855 switches provide high-density 400GE, 200GE, 100GE, 25GE, and 10GE ports and support power supply and fan module redundancy. You can deploy them in the new generation of data center core and aggregation networks. By connecting to upstream S12500 core switches through 400GE or 200GE links and to downstream access switches through 200GE, 100GE, or 40GE links, the S9825 and S9855 switches provide high bandwidth and large-capacity server access.
Technical specifications
Table1-1 Technical specifications
Item |
S9825-64D |
S9855-48CD8D |
S9855-24B8D |
S9855-40B |
S9855-32D |
Dimensions (H × W × D) |
175 × 440 × 760 mm (6.89 × 17.32 × 29.92 in) |
44 × 440 × 660 mm (1.73 × 17.32 × 25.98 in) |
44 × 440 × 550 mm (1.73 × 17.32 × 21.65 in) |
Weight |
LS-9825-64D: ≤ 37 kg (81.57 lb) LS-9825-64D-H1: ≤ 38.4 kg (84.66 lb) |
≤ 12.2 kg (26.90 lb) |
≤ 15.1 kg (33.29 lb) |
≤ 15.0 kg (33.07 lb) |
Serial console port |
1 |
1 |
1 |
1 |
1 |
Management Ethernet port (RJ-45) |
1 |
1 |
1 |
1 |
1 |
USB 2.0 port |
1 |
1 |
1 |
1 |
1 |
SFP+ port |
N/A |
N/A |
N/A |
N/A |
2 |
DSFP port |
N/A |
48 |
N/A |
N/A |
N/A |
QSFP56 port |
N/A |
N/A |
24 |
40 |
N/A |
QSFP-DD |
64 |
8 |
8 |
N/A |
32 |
Fan module slot |
LS-9825-64D: 6 LS-9825-64D-H1: 8 |
6 |
6 |
6 |
6 |
Power supply slot |
4 |
2 |
2 |
2 |
2 |
Minimum power consumption |
LS-9825-64D: · Dual AC inputs: 243 W · Four AC inputs: 251 W LS-9825-64D-H1: · Dual AC inputs: 247 W · Four AC inputs: 256 W |
Single AC input: 125 W Dual AC inputs: 140 W |
Single AC input: 133 W Dual AC inputs: 146 W |
Single AC input: 116 W Dual AC inputs: 127 W |
Single AC input: 199 W Single DC input: 221 W Dual AC inputs: 212 W Dual DC inputs: 234 W |
Typical power consumption |
LS-9825-64D: · Dual AC inputs: 613 W · Four AC inputs: 630 W LS-9825-64D-H1: · Dual AC inputs: 650 W · Four AC inputs: 680 W |
Single AC input: 238 W Dual AC inputs: 250 W |
Single AC input: 251 W Dual AC inputs: 263 W |
Single AC input: 246 W Dual AC inputs: 258 W |
Single AC input: 422 W Single DC input: 438 W Dual AC inputs: 439 W Dual DC inputs: 476 W |
Maximum power consumption |
LS-9825-64D: · Dual AC inputs: 1852 W · Four AC inputs: 1855 W LS-9825-64D-H1: · Dual AC inputs: 2500 W · Four AC inputs: 2500 W |
Single AC input: 713 W Dual AC inputs: 719 W |
Single AC input: 739 W Dual AC inputs: 748 W |
Single AC input: 706 W Dual AC inputs: 709 W |
Single AC input: 1096 W Single DC input: 1197 W Dual AC inputs: 1140 W Dual DC inputs: 1265 W |
Chassis leakage current compliance |
· UL60950-1 · EN60950-1 · IEC60950-1 · GB4943 |
Sound pressure level at 27°C (80.6°F) |
LS-9825-64D: 60.9 dB(A) LS-9825-64D-H1: 59.7 dB(A) |
59.5 dB(A) |
59.5 dB(A) |
52.8 dB(A) |
67.9 dB(A) |
Operating temperature |
0°C to 40°C (32°F to 104°F) |
Operating humidity |
5% RH to 95% RH, noncondensing |
Fire resistance compliance |
Table1-2 Power consumption data collection standard
Item |
Static power consumption |
Configuration |
No transceiver modules/cables installed in ports |
Fully configured with copper cables |
Fully configured with transceiver modules |
Load |
N/A |
50% load |
100% load |
2 Chassis views
S9825-64D
Figure2-1 S9825-64D front panel
(1) Management Ethernet port |
(2) Management Ethernet port LED (LINK/ACT) |
(3) USB port |
(4) Reset button (RESET) |
(5) QSFP-DD port |
(6) QSFP-DD port LED |
(7) System status LED (SYS) |
(8) Fan module status LED (FAN) |
(9) Power supply status LED (PSU) |
(10) Console port |
Figure2-2 S9825-64D rear panel (LS-9825-64D)
(1) Grounding screw |
(2) Fan module |
(3) Power output status LED (OUT) |
(4) Power input status LED (IN) |
(5) Power input receptacle |
(6) Power supply latch |
(7) Power supply fault LED (!) |
(8) Fan module alarm LED (RUN/ALM) |
The S9825-64D switch came with power supply slot PSU1 empty and power supply slots PSU2, PSU3, and PSU4 each installed with a filler panel. You can install two or multiple power supplies for the switch as needed. In Figure2-2, four PSR1600C-12A-B AC power supplies are installed in the power supply slots.
The S9825-64D switch model includes switches with the LS-9825-64D and LS-9825-64D-H1 product codes. The switch with the LS-S9825-64D product code came with the six fan module slots empty. The switch with the LS-9825-64D-H1 product code came with the eight fan module slots empty. You must install fan modules of the same model for the switch. In Figure2-2, six FAN-80B-1-B fan modules are installed in the fan module slots on the switch with the LS-S9825-64D product code.
Figure2-3 S9825-64D left panel
(1) Fan module handle |
(2) Power supply handle |
(3) Chassis handle |
S9855-48CD8D
Figure2-4 S9855-48CD8D front panel
(1) DSFP port |
(2) DSFP port LED |
(3) QSFP-DD port |
(4) QSFP-DD port LED |
(5) Fan module status LED (FAN) |
(6) Power supply status LED (PSU) |
Figure2-5 S9855-48CD8D rear panel
(2) USB port |
(3) Fan module |
(4) Fan module alarm LED |
(5) Power output status LED (OUT) |
(6) Power input status LED (IN) |
(7) Power input receptacle |
(8) Power supply latch |
(9) Power supply fault LED (!) |
(10) Reset button (RESET) |
(11) System status LED (SYS) |
(12) Console port |
(13) Management Ethernet port LED (LINK/ACT) |
The S9855-48CD8D switch came with power supply slot PSU1 empty and power supply slot PSU2 installed with a filler panel. You can install one or two power supplies for the switch as needed. In Figure2-5, two PSR1600C-12A-B AC power supplies are installed in the power supply slots.
The S9855-48CD8D switch came with the six fan module slots empty. You must install six fan modules of the same model for the switch. In Figure2-5, six FAN-40B-1-C fan modules are installed in the fan module slots.
Figure2-6 S9855-48CD8D left panel
(3) Primary grounding point |
(4) Auxiliary grounding point |
S9855-24B8D
Figure2-7 S9855-24B8D front panel
(1) System status LED (SYS) |
(2) Power supply status LED (PSU) |
(3) Fan module status LED (FAN) |
(4) QSFP56 port |
(5) QSFP56 port LED 1 |
(6) QSFP56 port LED 2 |
(7) QSFP-DD port LED |
(8) QSFP-DD port |
Figure2-8 S9855-24B8D rear panel
(2) USB port |
(3) Fan module |
(12) Console port |
The S9855-24B8D switch came with power supply slot PSU1 empty and power supply slot PSU2 installed with a filler panel. You can install one or two power supplies for the switch as needed. In Figure2-8, two PSR1600C-12A-B AC power supplies are installed in the power supply slots.
The S9855-24B8D switch came with the six fan module slots empty. You must install six fan modules of the same model for the switch. In Figure2-8, six FAN-40B-1-C fan modules are installed in the fan module slots.
Figure2-9 S9855-24B8D left panel
S9855-40B
Figure2-10 S9855-40B front panel
(2) Fan module status LED (FAN) |
(3) QSFP56 port LED |
(4) QSFP56 port |
(5) Device ID LED |
Figure2-11 S9855-40B rear panel
(1) Management Ethernet port LED (ACT) |
(2) Management Ethernet port |
(3) Management Ethernet port LED (LINK) |
(4) Fan module |
(5) Fan module alarm LED |
(6) Power supply fans |
(8) Power supply fault LED (!) |
(9) Power supply latch |
(10) Power supply handle |
(11) Console port |
(12) Device label pull tab (ASSET TAG) |
(13) USB port |
The S9855-40B switch came with power supply slot PSU1 empty and power supply slot PSU2 installed with a filler panel. You can install one or two power supplies for the switch as needed. In Figure2-11, two PSR1300-12A-C-B AC power supplies are installed in the power supply slots.
The S9855-40B switch came with the six fan module slots empty. You must install six fan modules of the same model for the switch. In Figure2-11, six FAN-40B-1-H fan modules are installed in the fan module slots.
Figure2-12 S9855-40B left panel
(2) Primary grounding point |
(3) Auxiliary grounding point |
(4) Power supply handle |
S9855-32D
Figure2-13 S9855-32D front panel
(1) Power supply status LED (PSU) |
(2) System status LED (SYS) |
(3) QSFP-DD port LED |
(4) QSFP-DD port |
(5) SFP+ port LED |
(6) SFP+ port |
(7) Fan module status LED (FAN) |
Figure2-14 S9855-32D rear panel
(2) USB port |
(3) Fan module |
(12) Console port |
The S9855-32D switch came with power supply slot PSU1 empty and power supply slot PSU2 installed with a filler panel. You can install one or two power supplies for the switch as needed. In Figure2-14, two PSR1600C-12A-B AC power supplies are installed in the power supply slots.
The S9855-32D switch came with the six fan module slots empty. You must install six fan modules of the same model for the switch. In Figure2-14, six FAN-40B-1-C fan modules are installed in the fan module slots.
Figure2-15 S9855-32D left panel
3 Removable components
The switch uses modular design. Table3-1 describes the removable components available for the switch.
Table3-1 Removable components available for the switch
Removable components |
BOM code |
S9825-64D |
S9855-48CD8D |
S9855-24B8D |
S9855-40B |
S9855-32D |
Power supplies |
PSR1600C-12A-B |
0231AFJ7 |
Supported |
Supported |
Supported |
Not supported |
Supported |
PSR1300-12A-C-B |
0231ALSR |
Not supported |
Not supported |
Not supported |
Supported |
Not supported |
PSR1300-12A-C-A |
0231ALSU |
Not supported |
Not supported |
Not supported |
Supported |
Not supported |
PSR2400B-12D-B |
0231AKV7 |
Supported |
Supported |
Supported |
Not supported |
Supported |
Fan modules |
FAN-80B-1-B |
0231ABV6 |
Supported |
Not supported |
Not supported |
Not supported |
Not supported |
FAN-40B-1-C |
0231AFJ9 |
Not supported |
Supported |
Supported |
Not supported |
Supported |
FAN-40F-1-D |
0231AKLC |
Not supported |
Not supported |
Supported |
Not supported |
Supported |
FAN-40B-1-H |
0231AMRK |
Not supported |
Not supported |
Not supported |
Supported |
Not supported |
The S9855-48CD8D, S9855-24B8D, S9855-40B, or S9855-32D switch can operate correctly with only one power supply. You can install two power supplies for 1+1 redundancy.
The S9825-64D switch can operate correctly with two power supplies. You can install three power supplies for 2+1 redundancy or four power supplies for 2+2 redundancy.
To ensure heat dissipation, make sure all fan module slots on the S9855-48CD8D, S9855-24B8D, S9855-40B, and S9855-32D switches have fan modules installed and the fan modules are the same model.
The S9825-64D switch with the LS-S9825-64D product code has six fan module slots. To ensure heat dissipation, make sure all fan module slots on the switch have fan modules installed and the fan modules are the same model.
The S9825-64D switch with the LS-9825-64D-H1 product code has eight fan module slots. When you install ZR or ZR+ modules in the two lower rows of ports on the switch, make sure all fan module slots on the switch have fan modules installed. In other situations, you can install six fan modules in slots FAN3 to FAN8.
Power supplies
WARNING! When the switch has power supplies in redundancy, you can replace a power supply without powering off the switch. To avoid device damage or bodily injury, make sure the power supply is powered off before you replace it. |
View
Figure3-1 PSR1600C-12A-B power supply
(1) Power supply fault LED (!) |
(2) Power output status LED (OUT) |
(3) Power input status LED (IN) |
(4) Power input receptacle |
(5) Latch |
(6) Handle |
For the LED description, see "Power supply LEDs."
Features
The PSR1600C-12A-B is a power supply with AC or HVDC input (240 VDC) and DC output. It provides a maximum output of 1600 W. Table3-2 describes the features provided by the PSR1600C-12A-B power supply.
Table3-2 PSR1600C-12A-B power supply features
Feature |
Protection function |
The power supply provides protection against input overcurrent, input undervoltage, output overcurrent, output overvoltage, output shortcircuit, and overtemperature conditions. |
Support for redundancy |
Multiple power supplies can be connected in parallel to achieve N+1 or N+N redundancy and load balancing. |
Support for hot swapping |
You can remove one of the power supplies in redundancy when the switch is operating. |
Table3-3 Technical specifications
Item |
Specification |
Net weight |
0.95 kg (2.09 lb) |
Rated AC input voltage range |
100 to 240 VAC @ 50 to 60 Hz |
Rated HVDC input voltage range |
180 to 320 VDC |
Output voltage |
12 V |
Max output current |
133 A |
Max output power |
1600 W |
Dimensions (H × W × D, including the handle) |
40.0 × 54.5 × 363.8 mm (1.57 × 2.15 × 14.32 in) |
–10°C to +55°C (14°F to 131°F) |
Operating relative humidity |
5% to 95% |
Airflow direction |
Draws air from the port side to the power supply side |
Melting current of power supply fuse |
10 A/250 V |
View
Figure3-2 PSR1300-12A-C-A power supply
(1) Handle |
(2) Velcro strap |
(3) Power input receptacle |
(4) Latch |
(5) LED |
Features
The PSR1300-12A-C-A is a power supply with AC or HVDC input (240 VDC) and DC output. It provides a maximum output of 1300 W. Table3-4 describes the features provided by the PSR1300-12A-C-A power supply.
Table3-4 PSR1300-12A-C-A power supply features
Feature |
Table3-5 Technical specifications
Item |
Specification |
Net weight |
0.90 kg (1.98 lb) |
180 to 320 VDC |
Output voltage |
12 V |
107 A |
Max output power |
1300 W |
40.0 × 73.5 × 185 mm (1.57 × 2.89 × 7.28 in) |
5% to 95% |
Airflow direction |
10 A/250 V |
View
Figure3-3 PSR1300-12A-C-B power supply
(1) Velcro strap |
(2) Handle |
(4) Latch |
(5) LED |
Features
The PSR1300-12A-C-B is a power supply with AC or HVDC input (240 VDC) and DC output. It provides a maximum output of 1300 W. Table3-6 describes the features provided by the PSR1300-12A-C-B power supply.
Table3-6 PSR1300-12A-C-B power supply features
Feature |
Table3-7 Technical specifications
Item |
Specification |
Net weight |
0.90 kg (1.98 lb) |
180 to 320 VDC |
Output voltage |
12 V |
107 A |
Max output power |
1300 W |
5% to 95% |
Airflow direction |
10 A/250 V |
View
Figure3-4 PSR2400B-12D-B power supply
(1) Power input negative connection |
(2) Power input positive connection |
(4) Power output status LED (OUT) |
(5) Power supply fault LED (!) |
(6) Handle |
(7) Latch |
Features
The PSR2400B-12D-B is a DC input and DC output power supply. It provides a maximum output of 2400 W. Table3-8 describes the features provided by the PSR2400B-12D-B power supply.
Table3-8 PSR2400B-12D-B power supply features
Feature |
Table3-9 Technical specifications
Item |
Specification |
Net weight |
1.05 kg (2.31 lb) |
Rated input voltage range |
–48 to –60 VDC |
Output voltage |
12 V |
200 A |
Max output power |
2400 W |
40.0 × 54.4 × 321.5 mm (1.57 × 2.14 × 12.66 in) |
–10°C to +50°C (14°F to 122°F) |
5% to 95% |
Airflow direction |
80 A/80 V |
Fan modules
FAN-80B-1-B
View
Figure3-5 FAN-80B-1-B fan module
(1) Handle |
(2) Alarm LED |
(3) Alignment hole |
Features
The FAN-80B-1-B fan module provides port-side intake and fan module faceplate-side exhaust airflow. The fan module is small, hot swappable, and can automatically adjust the fan speed according to the device temperature.
Table3-10 Technical specifications
Item |
Specification |
84 × 81 × 240 mm (3.31 × 3.19 × 9.45 in) |
Net weight |
0.90 kg (1.98 lb) |
Airflow direction |
Air exhausted from the faceplate |
Max fan speed |
12800 R.P.M |
Max air flow rate |
130 CFM (3.68 m3/min) |
Input voltage |
12 V |
Max power consumption |
102 W |
0°C to 45°C (32°F to 113°F) |
Storage temperature |
–40°C to +70°C (–40°F to +158°F) |
Storage relative humidity |
Hot swapping |
Supported |
FAN-40B-1-C
View
Figure3-6 FAN-40B-1-C fan module
For the LED description, see "Fan module alarm LED."
Features
The FAN-40B-1-C fan module provides port-side intake and fan module faceplate-side exhaust airflow. The fan module is small, hot swappable, and can automatically adjust the fan speed according to the device temperature.
Table3-11 Technical specifications
Item |
Specification |
40 × 40 × 136 mm (1.57 × 1.57 × 5.35 in) |
Weight |
0.15 kg (0.33 lb) |
Airflow direction |
Max fan speed |
29000 R.P.M |
Max air flow rate |
38 CFM (1.08 m3/min) |
Input voltage |
12 V |
60 W |
Hot swapping |
Supported |
FAN-40F-1-D
View
Figure3-7 FAN-40F-1-D fan module
Features
The FAN-40F-1-D fan module provides fan module faceplate-side intake and port-side exhaust airflow. The fan module is small, hot swappable, and can automatically adjust the fan speed according to the device temperature.
Table3-12 Technical specifications
Item |
Specification |
Weight |
0.15 kg (0.33 lb) |
Airflow direction |
Air exhausted from the port side |
Max fan speed |
29000 R.P.M |
Max air flow rate |
Input voltage |
12 V |
60 W |
Hot swapping |
Supported |
FAN-40B-1-H
View
Figure3-8 FAN-40B-1-H fan module
Functions
The FAN-40B-1-H fan module provides port-side intake and fan module faceplate-side exhaust airflow. The fan module is small, hot swappable, and can automatically adjust the fan speed according to the device temperature.
Table3-13 Technical specifications
Item |
Specification |
Weight |
0.15 kg (0.33 lb) |
Airflow direction |
Max fan speed |
28500/29000 R.P.M |
Max air flow rate |
Input voltage |
12 V |
60 W |
Hot swapping |
Supported |
4 Ports and LEDs
As a best practice, use H3C transceiver modules and cables for the switch. H3C transceiver modules and cables are subject to change over time. For the most up-to-date list of H3C transceiver modules and cables, contact H3C Support or marketing staff.
For information about the specifications of H3C transceiver modules and cables, see H3C Transceiver Modules User Guide.
Ports
Console port
The switch has a serial console port.
Table4-1 Console port specifications
Item |
Connector type |
RJ-45 |
Compliant standard |
EIA/TIA-232 |
Transmission baud rate |
9600 bps (default) to 115200 bps |
Services |
· Provides connection to an ASCII terminal. · Provides connection to the serial port of a local terminal (a PC for example) running a terminal emulation program. |
The switch has a copper management Ethernet port. You can connect the port to a local PC for software loading and debugging or to a remote management station for remote management.
Table4-2 Management Ethernet port specifications
Item |
Specification |
Connector type |
RJ-45 |
Port quantity |
1 × management 10/100/1000BASE-T port |
Port transmission rate, duplex mode, and auto MDI/MDI-X |
· 10/100 Mbps, half/full duplex, auto MDI/MDI-X · 1000 Mbps, full duplex, auto MDI/MDI-X |
Transmission medium and max transmission distance |
100 m (328.08 ft) over category 5 UTP cable |
Functions and services |
Software upgrade and network management. |
USB port
The switch has one OHCI-compliant USB 2.0 port that can upload and download data at a rate up to 480 Mbps. You can use this USB port to access the file system on the flash of the switch, for example, to upload or download application and configuration files.
The USB port supplies power as per USB 2.0 specifications. Use only USB 2.0-compliant USB devices for the USB port. The port might not identify USB devices that are not compliant with USB 2.0.
NOTE: USB devices from different vendors vary in compatibilities and drivers. H3C does not guarantee correct operation of USB devices of all vendors on the switch. If a USB device fails to operate on the switch, replace it with one from another vendor. |
SFP+ port
The S9855-32D switch provides two SFP+ ports on the front panel.
DSFP port
The S9855-48CD8D switch provides 48 DSFP ports on the front panel.
DSFP ports support the following transceiver modules and cables:
· SFP+ transceiver modules.
· SFP28 transceiver modules.
· SFP28 cables.
· DSFP transceiver modules.
· DSFP cables.
Purchase DSFP transceiver modules yourself as needed.
QSFP-DD port
The S9825-64D switch with the LS-9825-64D or LS-9825-64D-H1 product code provides 64 QSFP-DD ports. You can install ZR modules in the first row of ports on the switch. For the S9825-64D switch with the LS-9825-64D-H1 product code, you can also install ZR modules in the two lower rows of ports and ZR+ modules in the lowest row of ports. The 48 ports that support ZR modules on the switch are in pink.
The S9855-48CD8D and S9825-24B8D switches each provide eight QSFP-DD ports on the front panel.
The S9855-32D switch provides 32 QSFP-DD ports on the front panel.
QSFP-DD ports support the following transceiver modules and cables:
· QSFP28 transceiver modules.
· QSFP28 cables.
· QSFP56 transceiver modules.
· QSFP56 cables.
· QSFP-DD transceiver modules.
· QSFP-DD cables.
The eight QSFP-DD ports on the S9825-24B8D switch also support the following transceiver modules and cables:
· QSFP+ transceiver modules.
· QSFP+ cables.
· QSFP28 to 4 × 25G SFP28 cables.
The QSFP-DD ports on the S9855-32D switch also support QSFP+ modules and QSFP+ cables.
The QSFP-DD ports on the S9825-64D switch also support QSFP-DD to 2 × 200G QSFP56 cables. Such cables are not provided. Purchase them yourself as required.
QSFP56 port
The S9825-24B8D switch provides 24 QSFP56 ports.
The S9855-40B switch provides 40 QSFP56 ports.
QSFP56 ports support the following transceiver modules and cables:
· QSFP+ cables.
· QSFP+ to 4 × 10G SFP+ cables.
· QSFP28 cables.
· QSFP56 cables
· QSFP56 to 2 × 100G QSFP28 cables.
LEDs
Panel LEDs
System status LED
The system status LED shows the operating status of the switch.
Table4-3 System status LED description
LED mark |
Status |
SYS |
Steady green |
The switch is operating correctly. |
Flashing green |
The switch is performing power-on self-test (POST) or downloading software. |
Steady red |
The system has failed to pass POST, a fault has occurred, or an overtemperature condition has occurred. |
Steady yellow |
The number of fan modules or power supplies on the switch is abnormal. |
Off |
The switch is powered off or has failed to start up. |
DSFP port LED
The switch provides a DSFP port LED for each DSFP port to indicate their operating status.
Table4-4 DSFP port LED description
LED status |
Steady green |
A transceiver module or cable has been correctly installed in the port. The port is operating at its maximum speed of 100 Gbps, and a link is present on the port. |
Flashing green |
The port is sending or receiving data at its maximum speed of 100 Gbps. |
Steady yellow |
A transceiver module or cable has been correctly installed in the port. The port is operating at a speed lower than the maximum speed, and a link is present on the port. |
Flashing yellow |
The port is sending or receiving data at a speed lower than the maximum speed. |
Off |
No transceiver module or cable has been installed in the port, or no link is present on the port. |
QSFP56 port LED
Each QSFP56 port has two status LEDs to indicate port operating status and activities. Table4-5 provides the LED description for a QSFP56 port that is not split. Table4-6 provides the LED description for a QSFP56 port split into two breakout interfaces.
Table4-5 LED description for a QSFP56 port that is not split
LED status |
Steady green |
A transceiver module or cable has been correctly installed in the port. The port is operating at its maximum speed of 200 Gbps, and a link is present on the port. |
Flashing green |
The port is sending or receiving data at its maximum speed of 200 Gbps. |
Steady yellow |
Flashing yellow |
Off |
Table4-6 LED description for a QSFP56 port split into two breakout interfaces
LED status |
Steady green |
Flashing green |
Off |
NOTE: When the port is split into two breakout interfaces, QSFP56 port LED 1 indicates the operating status of the first breakout interface and QSFP56 port LED 2 indicates the operating status of the second breakout interface. For the LED description, see Table4-6. |
QSFP-DD port LED
The switch provides a QSFP-DD port LED for each QSFP-DD port to indicate their operating status.
Table4-7 QSFP-DD port LED description
LED status |
Steady green |
A transceiver module is installed in the port. The port is operating at its maximum speed of 400 Gbps, and a link is present on the port. |
Flashing green |
The port is sending or receiving data at its maximum speed of 400 Gbps. |
Steady yellow |
A transceiver module is installed in the port. The port is operating at a speed lower than the maximum speed, and a link is present on the port. |
Flashing yellow |
Off |
No transceiver module is installed in the port, or no link is present on the port. |
The switch provides a LINK/ACT LED for the copper management Ethernet port to indicate its operating status.
Table4-8 Management Ethernet port LED description
LED mark |
Status |
LINK/ACT |
Off |
No link is present on the port. |
Steady green |
The port is operating at 1000 Mbps. |
Flashing green |
The port is receiving or sending data at 1000 Mbps. |
Steady yellow |
The port is operating at 10/100 Mbps. |
Flashing yellow |
The port is receiving or sending data at 10/100 Mbps. |
The switch provides a fan module status LED for the fan modules to indicate their operating status.
Table4-9 Fan module status LED description
LED mark |
Status |
FAN |
Steady green |
All fan trays are operating correctly. |
Steady yellow |
A fan module is faulty or not in position. |
Steady red |
More than one fan module is faulty or not in position. |
The switch provides a power supply status LED for the power supplies to indicate their operating status.
Table4-10 Power supply status LED description
LED mark |
Status |
PSU |
Steady green |
All power supplies are operating correctly. |
Steady yellow |
A power supply is faulty or not in position. |
Steady red |
More than one power supply is faulty or not in position. |
The switch supports FAN-80B-1-B, FAN-40B-1-C, FAN-40F-1-D, and FAN-40B-1-H fan modules. Each fan module provides an alarm LED to indicate its operating status.
Table4-11 Description for the alarm LED on a fan module
Status |
Steady green |
The fan module is operating correctly. |
Steady red |
The fan module is faulty. |
Off |
The fan module is not securely installed or no power is present. |
Power supply LEDs
The switch supports the PSR1600C-12A-B, PSR2400B-12D-B, PSR1300-12A-C-B, and PSR1300-12A-C-A power supplies. Each power supply provides status LEDs to indicate its operating status. Table4-12 shows the description for the LEDs on a PSR1600C-12A-B or PSR2400B-12D-B power supply. Table4-13 shows the description for the LED on a PSR1300-12A-C-B or PSR1300-12A-C-A power supply.
Table4-12 Description for the LEDs on a PSR1600C-12A-B or PSR2400B-12D-B power supply
LED |
LED mark |
Status |
Power input status LED |
IN |
Steady green |
The power is being input correctly. |
Off |
No power is being input or the rated input voltage range has been exceeded. |
Power output status LED |
OUT |
Steady green |
The power is being output correctly. |
Off |
No power is being output. |
Power supply fault LED |
Flashing yellow |
The power supply is faulty. |
Off |
The power supply is operating correctly. |
Table4-13 Description for the LED on a PSR1300-12A-C-B or PSR1300-12A-C-A power supply
LED status |
Steady green |
Flashing green at 1 Hz |
The power supply is in standby state. |
Flashing green at 2 Hz |
The power supply is updating software. |
Flashing green at 0.33 Hz |
The power supply enters cold redundancy state. |
Steady amber |
The power supply does not have AC input, but the redundant power supply connected in parallel has normal power input. |
Flashing amber |
The power supply is operating correctly, but an overtemperature, overpower, overcurrent, or slow fan speed alarm has occurred. |
Off |
The power supply is not securely installed or has no power input. |
5 Cooling system
CAUTION: The chassis and power supplies use separate air aisles. Make sure the two aisles are not blocked when the switch is operating. |
The switch uses a highly efficient front-rear air aisle cooling system to ensure adequate heat dissipation and improve system reliability. Consider the ventilation design at the installation site when you plan the installation location for the switch.
Table5-1 Fan module options for the switch
Switch model |
Available fan module |
Airflow direction of the chassis |
S9825-64D |
FAN-80B-1-B |
From the port side to the power supply side |
S9855-48CD8D |
FAN-40B-1-C |
S9855-24B8D |
FAN-40B-1-C |
S9855-24B8D |
FAN-40F-1-D |
From the power supply side to the port side |
S9855-32D |
FAN-40B-1-C |
S9855-32D |
FAN-40F-1-D |
S9855-40B |
FAN-40B-1-H |
Figure5-1 Airflow from the port side to the power supply side through the S9825-64D chassis
Figure5-2 Airflow from the port side to the power supply side through the S9855-48CD8D chassis
Figure5-3 Airflow from the port side to the power supply side through the S9855-24B8D/S9855-32D chassis (S9855-24B8D chassis as an example)
Figure5-4 Airflow from the power supply side to the port side through the S9855-24B8D/S9855-32D chassis (S9855-24B8D chassis as an example)
Figure5-5 Airflow from the port side to the power supply side through the S9855-40B chassis