13-Layer 3—IP Services Command Reference
HomeSupportSecurityH3C SecPath F100-C-A FirewallReference GuidesCommand ReferencesH3C SecPath F100[F1000] Firewalls Series Command Reference(V7)-6W90013-Layer 3—IP Services Command Reference
08-DHCPv6 commands
08-DHCPv6 commands 487.02 KB
DHCPv6 commands· 1
Common DHCPv6 commands· 1
display ipv6 dhcp duid· 1
ipv6 dhcp dscp· 1
ipv6 dhcp log enable· 2
ipv6 dhcp select 2
DHCPv6 server commands· 3
address range· 3
class pool 5
default pool 5
display ipv6 dhcp option-group· 6
display ipv6 dhcp pool 8
display ipv6 dhcp prefix-pool 10
display ipv6 dhcp server 12
display ipv6 dhcp server conflict 13
display ipv6 dhcp server database· 14
display ipv6 dhcp server expired· 15
display ipv6 dhcp server ip-in-use· 16
display ipv6 dhcp server pd-in-use· 18
display ipv6 dhcp server statistics· 20
dns-server 22
domain-name· 23
if-match· 23
ipv6 dhcp advertise pd-route· 26
ipv6 dhcp apply-policy· 26
ipv6 dhcp class· 27
ipv6 dhcp option-group· 28
ipv6 dhcp policy· 29
ipv6 dhcp pool 29
ipv6 dhcp prefix-pool 30
ipv6 dhcp server 31
ipv6 dhcp server apply pool 32
ipv6 dhcp server database filename· 34
ipv6 dhcp server database update interval 35
ipv6 dhcp server database update now· 36
ipv6 dhcp server database update stop· 36
ipv6 dhcp server forbidden-address· 37
ipv6 dhcp server forbidden-prefix· 38
network· 39
option· 41
option-group· 42
prefix-pool 43
reset ipv6 dhcp server conflict 44
reset ipv6 dhcp server expired· 44
reset ipv6 dhcp server ip-in-use· 45
reset ipv6 dhcp server pd-in-use· 46
reset ipv6 dhcp server statistics· 47
sip-server 47
static-bind· 48
temporary address range· 49
vpn-instance· 50
DHCPv6 relay agent commands· 51
display ipv6 dhcp relay server-address· 51
display ipv6 dhcp relay statistics· 52
gateway-list 54
ipv6 dhcp relay client-link-address enable· 55
ipv6 dhcp relay gateway· 55
ipv6 dhcp relay interface-id· 56
ipv6 dhcp relay server-address· 57
remote-server 58
reset ipv6 dhcp relay statistics· 59
DHCPv6 client commands· 59
display ipv6 dhcp client 59
display ipv6 dhcp client statistics· 62
ipv6 address dhcp-alloc· 63
ipv6 dhcp client dscp· 64
ipv6 dhcp client duid· 65
ipv6 dhcp client pd· 66
ipv6 dhcp client stateful 67
ipv6 dhcp client stateless enable· 68
reset ipv6 dhcp client statistics· 68
DHCPv6 commands
Use display ipv6 dhcp duid to display the DUID of the local device.
context-admin
context-operator
A DHCP unique identifier (DUID) uniquely identifies a DHCPv6 device (DHCPv6 client, server, or relay agent). A DHCPv6 device adds its DUID in a sent packet.
This command displays output only after the DHCPv6 process is running on the device.
# Display the DUID of the local device.
<Sysname> display ipv6 dhcp duid
The DUID of this device: 0003000100e0fc005552.
ipv6 dhcp dscp
Use ipv6 dhcp dscp to set the DSCP value for the DHCPv6 packets sent by the DHCPv6 server or the DHCPv6 relay agent.
Use undo ipv6 dhcp dscp to restore the default.
ipv6 dhcp dscp dscp-value
undo ipv6 dhcp dscp
The DSCP value is 56 in DHCPv6 packets sent by the DHCPv6 server or the DHCPv6 relay agent.
context-admin
dscp-value: Specifies the DSCP value for DHCPv6 packets, in the range of 0 to 63.
The DSCP value of a packet specifies the priority level of the packet and affects the transmission priority of the packet. A bigger DSCP value represents a higher priority.
# Set the DSCP value to 30 for DHCPv6 packets sent by the DHCPv6 server or the DHCPv6 relay agent.
[Sysname] ipv6 dhcp dscp 30
Use ipv6 dhcp log enable to enable DHCPv6 server logging.
Use undo ipv6 dhcp log enable to disable DHCPv6 server logging.
DHCPv6 server logging is disabled.
context-admin
This command enables the DHCPv6 server to generate DHCPv6 logs and send them to the information center. The log information helps administrators locate and solve problems. For information about the log destination and output rule configuration in the information center, see Network Management and Monitoring Configuration Guide.
As a best practice, disable this feature if the log generation affects the device performance or reduces the address and prefix allocation efficiency. For example, this situation might occur when a large number of clients frequently come online or go offline.
# Enable DHCPv6 server logging.
[Sysname] ipv6 dhcp log enable
ipv6 dhcp select
Use ipv6 dhcp select to enable the DHCPv6 server or DHCPv6 relay agent on an interface.
Use undo ipv6 dhcp select to restore the default.
ipv6 dhcp select { relay | server }
An interface does not work in the DHCPv6 server mode or in the DHCPv6 relay agent mode. It discards DHCPv6 packets from DHCPv6 clients.
Interface view
context-admin
relay: Enables the DHCPv6 relay agent on the interface.
server: Enables the DHCPv6 server on the interface.
Before changing the DHCPv6 server mode to the DHCPv6 relay agent mode on an interface, use the following commands to remove IPv6 address/prefix bindings:
·     reset ipv6 dhcp server ip-in-use
·     reset ipv6 dhcp server pd-in-use
Do not configure the DHCPv6 client on the interface that has been configured as the DHCPv6 relay agent or DHCPv6 server.
# Enable the DHCPv6 server on GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp select server
# Enable the DHCPv6 relay agent on GigabitEthernet 1/0/2.
[Sysname-GigabitEthernet1/0/2] ipv6 dhcp select relay
address range
Use address range to specify a non-temporary IPv6 address range in a DHCPv6 address pool for dynamic allocation.
Use undo address range to restore the default.
address range start-ipv6-address end-ipv6-address [ preferred-lifetime preferred-lifetime valid-lifetime valid-lifetime ]
undo address range
No non-temporary IPv6 address range exists.
DHCPv6 address pool view
context-admin
start-ipv6-address: Specifies the start IPv6 address.
end-ipv6-address: Specifies the end IPv6 address.
preferred-lifetime preferred-lifetime: Specifies the preferred lifetime for the non-temporary IPv6 addresses. The value range is 60 to 4294967295 seconds, and the default is 604800 seconds (7 days).
valid-lifetime valid-lifetime: Specifies the valid lifetime for the non-temporary IPv6 addresses. The value range is 60 to 4294967295 seconds, and the default is 2592000 seconds (30 days). The valid lifetime cannot be shorter than the preferred lifetime.
If you do not specify a non-temporary IPv6 address range, all unicast addresses on the subnet specified by the network command in address pool view are assignable. If you specify a non-temporary IPv6 address range, only the IPv6 addresses in the specified IPv6 address range are assignable.
You can specify only one non-temporary IPv6 address range in an address pool. If you execute this command multiple times, the most recent configuration takes effect.
The non-temporary IPv6 address range specified by the address range command must be on the subnet specified by the network command.
# Configure a non-temporary IPv6 address range from 3ffe:501:ffff:100::10 through 3ffe:501:ffff:100::31 in address pool 1.
[Sysname] ipv6 dhcp pool 1
[Sysname-dhcp6-pool-1] network 3ffe:501:ffff:100::/64
[Sysname-dhcp6-pool-1] address range 3ffe:501:ffff:100::10 3ffe:501:ffff:100::31
network
class pool
Use class pool to specify a DHCPv6 address pool for a DHCPv6 user class.
Use undo class pool to restore the default.
class class-name pool pool-name
undo class class-name pool
No DHCPv6 address pool is specified for a DHCPv6 user class.
DHCPv6 policy view
context-admin
class-name: Specifies a DHCPv6 user class by its name, a case-insensitive string of 1 to 63 characters.
pool-name: Specifies a DHCPv6 address pool by its name, a case-insensitive string of 1 to 63 characters.
You can specify only one DHCPv6 address pool for a DHCPv6 user class in a DHCPv6 policy. If you execute this command multiple times for a user class, the most recent configuration takes effect.
# Specify DHCPv6 address pool pool1 for DHCPv6 user class test in DHCPv6 policy 1.
[Sysname] ipv6 dhcp policy 1
[Sysname-dhcp6-policy-1] class test pool pool1
default pool
ipv6 dhcp policy
ipv6 dhcp pool
default pool
Use default pool to specify the default DHCPv6 address pool.
Use undo default pool to restore the default.
default pool pool-name
undo default pool
No default DHCPv6 address pool is specified.
DHCPv6 policy view
context-admin
In a DHCPv6 policy, the DHCPv6 server uses the default address pool to assign IPv6 address, IPv6 prefix, or other parameters to clients that do not match any user classes. If no default address pool is specified or the default address pool does not have assignable IPv6 addresses or prefixes, the assignment fails.
You can specify only one default address pool in a DHCPv6 policy. If you execute this command multiple times, the most recent configuration takes effect.
# Specify the DHCPv6 address pool pool1 as the default DHCPv6 address pool in DHCPv6 policy 1.
[Sysname-dhcp6-policy-1] default pool pool1
class pool
ipv6 dhcp policy
Use display ipv6 dhcp option-group to display information about a DHCPv6 option group.
display ipv6 dhcp option-group [ option-group-number ]
context-admin
context-operator
option-group-number: Specifies a static or dynamic DHCPv6 option group by its ID. The value range for the option group ID is 1 to 100. If you do not specify an option group, this command displays information about all DHCPv6 option groups.
A static DHCPv6 option group is created by using the ipv6 dhcp option-group command.
A dynamic DHCPv6 option group is created automatically by a DHCPv6 client after it obtains the DHCPv6 configuration parameters. Dynamic option groups cannot be manually modified or deleted.
# Display information about all DHCPv6 option groups.
<Sysname> display ipv6 dhcp option-group
DHCPv6 option group: 1
  DNS server addresses:
    Type: Static
    Interface: N/A
    1::1
    Type: Dynamic (DHCPv6 address allocation)
    1::1
  Domain name:
    Type: Static
    Interface: N/A
    aaa.example.com
  Domain name:
    aaa.example.com
  Options:
    Code: 23
      Type: Dynamic (DHCPv6 prefix allocation)
      Length: 2 bytes
      Hex: ABCD
DHCPv6 option group: 20
    Type: Static
    Interface: N/A
    1::1
    1::1
  Domain name:
    Type: Static
    Interface: N/A
    aaa.example.com
  Domain name:
    aaa.example.com
  Options:
    Code: 23
      Length: 2 bytes
      Hex: ABCD
DHCPv6 option group
ID of the DHCPv6 option group.
Types of the DHCPv6 option:
·     StaticParameter in a static DHCPv6 option group.
·     Dynamic (DHCPv6 address allocation)—Parameter in a dynamic DHCPv6 option group created during IPv6 address acquisition.
·     Dynamic (DHCPv6 prefix allocation)—Parameters in a dynamic DHCPv6 option group created during IPv6 prefix acquisition.
·     Dynamic (DHCPv6 address and prefix allocation)—Parameters in a dynamic DHCPv6 option group created during IPv6 address and prefix acquisition.
Interface name.
IPv6 address of the DNS server.
Domain name
Domain name suffix.
SIP server addresses
IPv6 address of the SIP server.
SIP server domain names
Domain name of the SIP server.
Options
Self-defined options.
Code
Code of the self-defined option.
Length
Self-defined option length in bytes.
Hex
Self-defined option content represented by a hexadecimal number.
Use display ipv6 dhcp pool to display information about a DHCPv6 address pool.
display ipv6 dhcp pool [ pool-name | vpn-instance vpn-instance-name ]
context-admin
context-operator
pool-name: Displays information about the specified DHCPv6 address pool. The pool name is a case-insensitive string of 1 to 63 characters. If you do not specify a DHCPv6 address pool, this command displays information about all DHCPv6 address pools.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays information about DHCPv6 address pools for the public network.
# Display information about DHCPv6 address pool 1.
<Sysname> display ipv6 dhcp pool 1
DHCPv6 pool: 1
  Network: 3FFE:501:FFFF:100::/64
    Preferred lifetime 604800 seconds, valid lifetime 2592000 seconds
  Prefix pool: 1
    Preferred lifetime 24000 seconds, valid lifetime 36000 seconds
  Addresses:
    Range: from 3FFE:501:FFFF:100::1
           to 3FFE:501:FFFF:100::99
    Preferred lifetime 70480 seconds, valid lifetime 200000 seconds
    Total address number: 153
    Available: 153
    In-use: 0
  Temporary addresses:
    Range: from 3FFE:501:FFFF:100::200
           to 3FFE:501:FFFF:100::210
    Preferred lifetime 60480 seconds, valid lifetime 259200 seconds
    Total address number: 17
    Available: 17
    In-use: 0
  Static bindings:
    DUID: 0003000100e0fc000001
    IAID: 0000003f
    Prefix: 3FFE:501:FFFF:200::/64
    Description: ClientA
    DUID: 0003000100e0fc00cff1
    IAID: 00000001
    Address: 3FFE:501:FFFF:2001::1/64
    Description: ClientB
    2::2
  Domain name:
    aaa.example.com
  SIP server addresses:
    5::1
  SIP server domain names:
    bbb.example.com
DHCPv6 pool: 1
  Network: Not-available
DHCPv6 pool: 1
  Network: 1::/64(Zombie)
DHCPv6 pool
Name of the DHCPv6 address pool.
Network
IPv6 subnet for dynamic IPv6 address allocation.
If the subnet prefix is ineffective, this field displays Not-available. If the subnet prefix becomes ineffective after a configuration recovery (for example, a switchover from the backup to the master), the prefix is marked (Zombie).
Prefix pool
Prefix pool referenced by the address pool.
Preferred lifetime
Preferred lifetime in seconds.
valid lifetime
Valid lifetime in seconds.
Addresses
Non-temporary IPv6 address range.
Range
IPv6 address range for dynamic allocation.
Total number of IPv6 addresses.
Available
Total number of available IPv6 addresses.
In-use
Total number of assigned IPv6 addresses.
Temporary addresses
Temporary IPv6 address range for dynamic allocation.
Static bindings
Static bindings configured in the address pool.
DUID
Client DUID.
IAID
Client IAID. If no IAID is configured, this field displays Not configured.
Prefix
IPv6 address prefix.
Address
Static IPv6 address.
Description of the static binding.
DNS server address.
Domain name
Domain name.
SIP server address.
Use display ipv6 dhcp prefix-pool to display information about a prefix pool.
display ipv6 dhcp prefix-pool [ prefix-pool-number ] [ vpn-instance vpn-instance-name ]
context-admin
context-operator
prefix-pool-number: Displays detailed information about a prefix pool specified by its number in the range of 1 to 128. If you do not specify a prefix pool, this command displays brief information about all prefix pools.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays information about prefix pools for the public network.
# Display brief information about all prefix pools.
<Sysname> display ipv6 dhcp prefix-pool
Prefix-pool Prefix                                      Available In-use Static
1           5::/64                                      64        0      0
2           Not-available                               0         0      0
11          21::/112(Zombie)                            0         64     0
# Display detailed information about prefix pool 1.
<Sysname> display ipv6 dhcp prefix-pool 1
Prefix: 5::/64
Assigned length: 70
Total prefix number: 64
Available: 64
In-use: 0
Static: 0
Prefix: Not-available
Assigned length: 70
Total prefix number: 0
Available: 0
In-use: 0
Static: 0
Prefix: 5::/64(Zombie)
Assigned length: 70
Total prefix number: 10
Available: 0
In-use: 10
Static: 0
Prefix-pool
Prefix pool number.
Prefix
Prefix specified in the prefix pool.
If the prefix is ineffective, this field displays Not-available. If the prefix becomes ineffective after a configuration recovery (for example, a switchover from the backup to the master), the prefix is marked (Zombie).
Available
Number of available prefixes.
In-use
Number of assigned prefixes.
Static
Number of statically bound prefixes.
Assigned length
Length of assigned prefixes.
Total prefix number
Number of prefixes.
Use display ipv6 dhcp server to display DHCPv6 server configuration information.
display ipv6 dhcp server [ interface interface-type interface-number ]
context-admin
context-operator
interface interface-type interface-number: Displays DHCPv6 server configuration information for the specified interface. If you do not specify an interface, this command displays DHCPv6 server configuration information for all interfaces.
# Display DHCPv6 server configuration information for all interfaces.
<Sysname> display ipv6 dhcp server
Interface             Pool
GigabitEthernet1/0/1  1
GigabitEthernet1/0/2  global
# Display DHCPv6 server configuration information for the interface GigabitEthernet 1/0/1.
<Sysname> display ipv6 dhcp server interface gigabitethernet 1/0/1
Using pool: 1
Preference value: 0
Allow-hint: Enabled
Rapid-commit: Disabled
Interface enabled with DHCPv6 server.
Pool
Address pool applied to the interface.
If no address pool is applied to the interface, global is displayed. The DHCPv6 server selects a global address pool to assign a prefix, an address, and other configuration parameters to a client.
Using pool
Preference value
Server preference in the DHCPv6 Advertise message. The value range is 0 to 255. The bigger the value is, the higher preference the server has.
Allow-hint
Indicates whether desired address/prefix assignment is enabled.
Rapid-commit
Indicates whether rapid address/prefix assignment is enabled.
Use display ipv6 dhcp server conflict to display information about IPv6 address conflicts.
display ipv6 dhcp server conflict [ address ipv6-address ] [ vpn-instance vpn-instance-name ]
context-admin
context-operator
address ipv6-address: Displays conflict information for the specified IPv6 address. If you do not specify an IPv6 address, this command displays information about all IPv6 address conflicts.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays IPv6 address conflict information for the public network.
The DHCPv6 server creates IP address conflict information in the following conditions:
·     The DHCPv6 client sends a DECLINE packet to the DHCPv6 server to inform the server of an IPv6 address conflict.
·     The DHCPv6 server discovers that the only assignable address in the address pool is its own IPv6 address.
# Display information about all address conflicts.
<Sysname> display ipv6 dhcp server conflict
IPv6 address                                 Detect time
2001::1                                      Apr 25 16:57:20 2019
1::1:2                                       Apr 25 17:00:10 2019
Table 5 Command output
IPv6 address
Conflicted IPv6 address.
Detect time
Time when the conflict was discovered.
Use display ipv6 dhcp server database to display information about DHCPv6 binding auto backup.
context-admin
context-operator
# Display information about DHCPv6 binding auto backup.
<Sysname> display ipv6 dhcp server database
 Username                :
 Password                :
 Latest write time       :   Feb  8 16:02:23 2014
Table 6 Command output
File name
Name of the DHCPv6 binding backup file.
Username
Username for accessing the URL of the remote backup file.
Password
Password for accessing the URL of the remote backup file. This field displays ****** if a password is configured.
Update interval
Waiting time in seconds after a DHCPv6 binding change for the DHCPv6 server to update the backup file.
Latest write time
Time of the latest update.
Status
Status of the update:
·     Writing—The backup file is being updated.
·     Last write succeeded—The backup file was successfully updated.
·     Last write failed—The backup file failed to be updated.
Use display ipv6 dhcp server expired to display lease expiration information.
display ipv6 dhcp server expired [ [ address ipv6-address ] [ vpn-instance vpn-instance-name ] | pool pool-name ]
context-admin
context-operator
address ipv6-address: Displays lease expiration information for the specified IPv6 address. If you do not specify an IPv6 address, this command displays lease expiration information for all IPv6 addresses.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays lease expiration information about IPv6 addresses for the public network.
pool pool-name: Displays lease expiration information for the DHCPv6 address pool specified by its name, a case-insensitive string of 1 to 63 characters. If you do not specify a DHCPv6 address pool, this command displays lease expiration information for all DHCPv6 address pools.
DHCPv6 assigns the expired IPv6 addresses to DHCPv6 clients when all available addresses have been assigned.
# Display all lease expiration information.
<Sysname> display ipv6 dhcp server expired
IPv6 address           DUID                            Lease expiration
2001:3eff:fe80:4caa:   3030-3066-2e65-3230-302e-       Apr 25 17:10:47 2019
37ee:7::1              3130-3234-2d45-7468-6572-
                       6e65-7430-2f31
Table 7 Command output
IPv6 address
Expired IPv6 address.
DUID
Client DUID bound to the expired IPv6 address.
Lease expiration
Time when the lease expired.
Use display ipv6 dhcp server ip-in-use to display binding information for assigned IPv6 addresses.
display ipv6 dhcp server ip-in-use [ [ address ipv6-address ] [ vpn-instance vpn-instance-name ] | pool pool-name ]
context-admin
context-operator
address ipv6-address: Displays binding information for the specified IPv6 address. If you do not specify an IPv6 address, this command displays binding information for all IPv6 addresses.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays binding information about IPv6 addresses for the public network.
pool pool-name: Displays IPv6 address binding information for the DHCPv6 address pool specified by its name, a case-insensitive string of 1 to 63 characters. If you do not specify a DHCPv6 address pool, this command displays IPv6 address binding information for all DHCPv6 address pools.
# Display binding information for all assigned IPv6 address.
<Sysname> display ipv6 dhcp server ip-in-use
Pool: 1
 IPv6 address            Hardware address     Type      Lease expiration
 2:1::1                  0125-0354-aab2       Auto(O)   Jul 10 19:45:01 2019
Pool: 2
 1:1::2                  1325-0714-a3ec       Static(F) Not available
Pool: 3
 1:2::1F1                bb43-1314-bb32       Static(O) Oct  9 09:23:31 2019
Pool: 4
 2001:2F01:3EE3:3200:    ac22-5456-ee76       Auto(Z)   Oct  11 09:23:31 2019
 E013:7A86:5905:2012
# Display binding information for all assigned IPv6 addresses for the specified DHCPv6 address pool.
<Sysname> display ipv6 dhcp server ip-in-use pool 1
Pool: 1
 2:1::1                  0125-0354-aab2       Auto(O)   Jul 10 22:22:22 2019
 3:1::2                  1563-8654-e2a3       Static(C) Jan  1 11:11:11 2019
# Display binding information for the specified IPv6 address.
<Sysname> display ipv6 dhcp server ip-in-use address 2:1::3
Pool: 1
Client: FE80::C800:CFF0:FE18:0
Hardware address: 3674-0832-eab3
Type: Auto(O)
DUID: 00030001CA000C180000
IAID: 0x00030001
  IPv6 address: 2:1::3
  Preferred lifetime 400 seconds, valid lifetime 500 seconds
  Expires at Jul 10 09:45:01 2019 (288 seconds left)
Table 8 Command output
Pool
IPv6 address
IPv6 address assigned.
Hardware address
Hardware address of a DHCPv6 client. In a network with DHCPv6 relay agent, this field displays N/A because the DHCPv6 server cannot obtain the hardware address of the client.
IPv6 address binding types:
·     Static(F)—Free static binding whose IPv6 address has not been assigned.
·     Static(O)—Offered static binding whose IPv6 address has been selected and sent by the DHCPv6 server in a DHCPv6-OFFER packet to the client.
·     Static(C)—Committed static binding whose IPv6 address has been assigned to the client.
·     Auto(O)—Offered dynamic binding whose IPv6 address has been dynamically selected by the DHCPv6 server and sent in a DHCPv6-OFFER packet to the DHCPv6 client.
·     Auto(C)—Committed dynamic binding whose IPv6 address has been dynamically assigned to the DHCPv6 client.
·     Auto(Z)—Zombie dynamic binding whose IPv6 address has been dynamically assigned to the DHCPv6 client. The binding becomes zombie because the subnet prefix goes invalid for address allocation after a configuration recovery, for example, after a switchover from the backup to the master.
Lease-expiration
Time when the lease of the IPv6 address will expire. If the lease expires after the year 2100, this field displays Expires after 2100. For an unassigned static binding, this field displays Not available.
Client
IPv6 address of the DHCPv6 client. For an unassigned static binding, this field is blank.
DUID
Client DUID.
IAID
Client IAID. For an unassigned static binding without IAID specified, this field displays N/A.
Preferred lifetime
Preferred lifetime in seconds of the IPv6 address.
valid lifetime
Valid lifetime in seconds of the IPv6 address.
Expires at
Time when the lease of an IPv6 address will expire. If the lease expires after the year 2100, this field displays Expires after 2100.
Use display ipv6 dhcp server pd-in-use to display binding information for the assigned IPv6 prefixes.
display ipv6 dhcp server pd-in-use [ pool pool-name | [ prefix prefix/prefix-len ] [ vpn-instance vpn-instance-name ] ]
context-admin
context-operator
pool pool-name: Displays IPv6 prefix binding information for the DHCPv6 address pool specified by its name, a case-insensitive string of 1 to 63 characters. If you do not specify a DHCPv6 address pool, this command displays IPv6 prefix binding information for all DHCPv6 address pools.
prefix prefix/prefix-len: Displays binding information for the specified IPv6 prefix. The value range for the prefix length is 1 to 128. If you do not specify an IPv6 prefix, this command displays binding information for all IPv6 prefixes.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays binding information about IPv6 prefixes for the public network.
# Display all IPv6 prefix binding information.
<Sysname> display ipv6 dhcp server pd-in-use
Pool: 1
 IPv6 prefix             Hardware address     Type      Lease expiration
 2:1::/24                0125-0354-aab2       Auto(O)   Jul 10 19:45:01 2019
Pool: 2
 1:1::/64                1325-0714-a3ec       Static(F) Not available
Pool: 3
 1:2::/64                bb43-1314-bb32       Static(O) Oct  9 09:23:31 2019
Pool: 4
 12::/80                 ac22-5456-ee76       Auto(Z)   Oct 17 09:34:59 2019
# Display IPv6 prefix binding information for DHCPv6 address pool 1.
<Sysname> display ipv6 dhcp server pd-in-use pool 1
Pool: 1
 2:1::/24                0125-0354-aab2       Auto(O)   Jul 10 22:22:22 2019
 3:1::/64                1563-8654-e2a3       Static(C) Jan  1 11:11:11 2019
# Display binding information for the IPv6 prefix 2:1::3/24.
<Sysname> display ipv6 dhcp server pd-in-use prefix 2:1::3/24
Pool: 1
Client: FE80::C800:CFF:FE18:0
Type: Auto(O)
IAID: 0x00030001
  IPv6 prefix: 2:1::/24
Table 9 Command output
IPv6 prefix
IPv6 prefix assigned.
Hardware address
Prefix binding types:
·     Static(F)—Free static binding whose IPv6 prefix has not been assigned.
·     Static(O)—Offered static binding whose IPv6 prefix has been selected and sent by the DHCPv6 server in a DHCPv6-OFFER packet to the client.
·     Static(C)—Committed static binding whose IPv6 prefix has been assigned to the client.
·     Auto(O)—Offered dynamic binding whose IPv6 prefix has been dynamically selected by the DHCPv6 server and sent in a DHCPv6-OFFER packet to the DHCPv6 client.
·     Auto(C)—Committed dynamic binding whose IPv6 prefix has been dynamically assigned to the DHCPv6 client.
·     Auto(Z)—Zombie dynamic binding whose IPv6 prefix has been dynamically assigned to the DHCPv6 client. The binding becomes zombie because the prefix in the prefix pool goes invalid after a configuration recovery, for example, after a switchover from the backup to the master.
Pool
Address pool.
Lease-expiration
Time when the lease of the IPv6 prefix will expire. If the lease will expire after the year 2100, this field displays Expires after 2100. For an unassigned static binding, this field displays Not available.
Client
DUID
Client DUID.
IAID
Client IAID. For an unassigned static binding without IAID, this field displays N/A.
Preferred lifetime
Preferred lifetime in seconds of the IPv6 prefix.
valid lifetime
Valid lifetime in seconds of the IPv6 prefix.
Expires at
Time when the lease of the prefix will expire. If the lease expires after the year 2100, this field displays Expires after 2100.
Use display ipv6 dhcp server statistics to display DHCPv6 packet statistics on the DHCPv6 server.
display ipv6 dhcp server statistics [ pool pool-name | vpn-instance vpn-instance-name ]
context-admin
context-operator
pool pool-name: Displays DHCPv6 packet statistics for the DHCPv6 address pool specified by its name, a case-insensitive string of 1 to 63 characters. If you do not specify an address pool, this command displays DHCPv6 packet statistics for all address pools.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays DHCPv6 server statistics for the public network.
# Display all DHCPv6 packet statistics on the DHCPv6 server.
<Sysname> display ipv6 dhcp server statistics
Bindings:
    Ip-in-use                 :  1
    Pd-in-use                 :  0
    Expired                   :  0
Conflict                      :  0
Packets received              :  1
    Solicit                   :  1
    Request                   :  0
    Confirm                   :  0
    Renew                     :  0
    Rebind                    :  0
    Release                   :  0
    Decline                   :  0
    Information-request       :  0
    Relay-forward             :  0
Packets dropped               :  0
Packets sent                  :  0
    Advertise                 :  0
    Reconfigure               :  0
    Reply                     :  0
    Relay-reply               :  0
Table 10 Command output
Bindings
Number of bindings:
·     Ip-in-use—Total number of address bindings.
·     Pd-in-use—Total number of prefix bindings.
·     Expired—Total number of expired address bindings.
Conflict
Total number of conflicted addresses. If statistics about an address pool are displayed, this field is not displayed.
Packets received
Number of messages received by the DHCPv6 server. The message types include:
·     Solicit.
·     Request.
·     Confirm.
·     Renew.
·     Rebind.
·     Release.
·     Decline.
·     Information-request.
·     Relay-forward.
Packets dropped
Number of packets discarded. If statistics about an address pool are displayed, this field is not displayed.
Packets sent
Number of messages sent by the DHCPv6 server. The message types include:
·     Advertise.
·     Reconfigure.
·     Reply.
·     Relay-reply.
dns-server
Use dns-server to specify a DNS server in a DHCPv6 address pool.
Use undo dns-server to remove the specified DNS server from a DHCPv6 address pool.
dns-server ipv6-address
undo dns-server ipv6-address
No DNS server address is specified.
DHCPv6 option group view
context-admin
ipv6-address: Specifies the IPv6 address of a DNS server.
You can use the dns-server command to specify up to eight DNS servers in an address pool. A DNS server specified earlier has a higher preference.
# Specify the DNS server address 2:2::3 in DHCPv6 address pool 1.
[Sysname-dhcp6-pool-1] dns-server 2:2::3
domain-name
Use domain-name to specify a domain name in a DHCPv6 address pool.
Use undo domain-name to restore the default.
domain-name domain-name
undo domain-name
No domain name is specified.
context-admin
domain-name: Specifies a domain name, a case-sensitive string of 1 to 50 characters.
You can configure only one domain name in an address pool. If you execute this command multiple times, the most recent configuration takes effect.
# Specify the domain name aaa.example.com in DHCPv6 address pool 1.
[Sysname-dhcp6-pool-1] domain-name aaa.example.com
if-match
Use if-match to configure a match rule for a DHCPv6 user class.
Use undo if-match to delete a match rule for a DHCP user class.
if-match rule rule-number { option option-code [ ascii ascii-string [ offset offset | partial ] | hex hex-string [ mask mask | offset offset length length | partial ] ] | relay-agent gateway-ipv6-address }
No match rules are configured for the DHCPv6 user class.
DHCPv6 user class view
context-admin
rule rule-number: Assigns the match rule an ID in the range of 1 to 128. A smaller ID represents a higher match priority.
option option-code: Specifies a DHCPv6 option by its number in the range of 1 to 65535.
ascii ascii-string: Specifies an ASCII string of 1 to 128 characters.
offset offset: Specifies the offset in bytes after which the match operation starts. The value range is 0 to 65534. If you specify an ASCII string, a packet matches the rule if the option content after the offset is the same as the ASCII string. If you specify a hexadecimal number, a packet matches the rule if the option content of the specified length after the offset is the same as the hexadecimal number.
partial: Enables partial match. A packet matches the rule if the specified option in the packet contains the ASCII string or hexadecimal number specified in the rule. For example, if you specify abc in the rule, option content xabc, xyzabca, xabcyz, and abcxyz all match the rule.
hex hex-string: Specifies a hexadecimal number. The length of the hexadecimal number must be an even number in the range of 2 to 256.
mask mask: Specifies the mask for the match operation. The mask is a hexadecimal number whose length is an even number in the range of 2 to 256 and must be the same as the hex-string length. The DHCPv6 server selects option content of the mask length from the start and ANDs the selected option content and the specified hexadecimal number with the mask. The packet matches the rule if the two AND operation results are the same.
length length: Specifies the length of the option content to be matched, in the range of 1 to 128 bytes. The length must be the same as the hex-string length.
relay-agent gateway-ipv6-address: Specifies a link-address field value. The value is an IPv6 address. A packet matches the rule if its link-address field value is the same as that in the rule.
If a DHCPv6 request sent by a DHCPv6 client matches a rule in a DHCPv6 user class, the DHCPv6 client matches the user class.
You can configure multiple match rules for a DHCPv6 user class. Each match rule is uniquely identified by a rule ID within its type (option or relay agent address).
·     If the rule that you are configuring has the same ID and type as an existing rule, the new rule overwrites the existing rule.
·     If the rule that you are configuring has the same ID as an existing rule but a different type, the new rule takes effect and coexists with the existing rule. As a best practice, do not assign the same ID to rules of different types.
·     Rules of different IDs cannot have the same rule content.
When you configure an if-match option rule, follow these guidelines:
·     To match packets that contain an option, specify only the option-code argument.
·     To match a hexadecimal number by AND operations, specify the option option-code hex hex-string mask mask options.
·     To match a hexadecimal number directly, specify the option option-code hex hex-string [ offset offset length length | partial ] options. If you do not specify the offset, length, or partial parameter, a packet matches a rule if the option content starts with the hexadecimal number.
·     To match an ASCII string, specify the option option-code ascii ascii-string [ offset offset | partial ] options. If you do not specify the offset or partial parameter, a packet matches a rule if the option content starts with the ASCII string.
# Configure match rule 1 for the DHCPv6 user class exam to match DHCPv6 requests that contain Option 16.
[Sysname] ipv6 dhcp class exam
[Sysname-dhcp6-class-exam] if-match rule 1 option 16
# Configure match rule 2 for the DHCPv6 user class exam. The rule matches DHCPv6 requests in which the highest bit of the fourth byte in Option 16 is the hexadecimal number 1.
[Sysname-dhcp6-class-exam] if-match rule 2 option 16 hex 00000080 mask 00000080
# Configure match rule 3 for the DHCPv6 user class exam. The rule matches DHCPv6 requests in which the first three bytes of Option 16 are the hexadecimal number 13ae92.
[Sysname-dhcp6-class-exam] if-match rule 3 option 16 hex 13ae92 offset 0 length 3
# Configure match rule 4 for the DHCPv6 user class exam. The rule matches DHCPv6 requests in which the Option 16 contains the hexadecimal number 13ae.
[Sysname-dhcp6-class-exam] if-match rule 5 option 16 hex 13ae partial
# Configure match rule 5 for the DHCPv6 user class exam to match DHCPv6 requests in which the link-address field is 2001::1.
[Sysname-dhcp6-class-exam] if-match rule 5 relay-agent 2001::1
ipv6 dhcp class
Use ipv6 dhcp advertise pd-route to enable the DHCPv6 server to advertise routes for the IPv6 prefixes assigned to directly connected clients.
Use undo ipv6 dhcp advertise pd-route to disable the DHCPv6 server from advertising routes for the IPv6 prefixes assigned to directly connected clients.
The DHCPv6 server does not advertise routes for the IPv6 prefixes assigned to directly connected clients.
context-admin
A DHCPv6 client can obtain an IPv6 prefix through DHCPv6 and use this IPv6 prefix to assign IPv6 addresses to hosts in a downstream network. A host in the downstream network cannot access the external network if the following conditions exist:
·     The DHCPv6 client is directly connected to the DHCPv6 server, but the client does not run on the same subnet as the host.
·     The network-side device does not have a route to the host.
To resolve this issue, use this feature on the DHCPv6 server. This feature enables the DHCPv6 server to generate a routing entry for the IPv6 prefix and advertises this entry to the dynamic routing protocol. When the external network device learns this route through the dynamic routing protocol, it can communicate with the hosts in the downstream network.
To prevent the network-side device from accessing the hosts in downstream network, disable this feature.
# Enable the DHCPv6 server from advertising routes for the IPv6 prefixes assigned to directly connected clients.
[Sysname] ipv6 dhcp advertise pd-route
Use ipv6 dhcp apply-policy to apply a DHCPv6 policy to an interface.
Use undo ipv6 dhcp apply-policy to restore the default.
ipv6 dhcp apply-policy policy-name
No DHCPv6 policy is applied to an interface.
Interface view
context-admin
policy-name: Specifies a DHCPv6 policy by its name, a case-insensitive string of 1 to 63 characters.
You can apply only one DHCPv6 policy to an interface. If you execute this command multiple times, the most recent configuration takes effect.
# Apply the DHCPv6 policy test to GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp apply-policy test
ipv6 dhcp class
ipv6 dhcp class
Use ipv6 dhcp class to create a DHCPv6 user class and enter its view, or enter the view of an existing DHCPv6 user class.
Use undo ipv6 dhcp class to delete the specified DHCPv6 user class.
ipv6 dhcp class class-name
undo ipv6 dhcp class class-name
No DHCPv6 user classes exist.
context-admin
class-name: Specifies a name for the DHCPv6 user class, a case-insensitive string of 1 to 63 characters.
In the DHCPv6 user class view, you can use the if-match command to configure match rules for user classification.
# Create a DHCPv6 user class test and enter DHCPv6 user class view.
[Sysname] ipv6 dhcp class test
[Sysname-dhcp6-class-test]
class pool
ipv6 dhcp policy
if-match
Use ipv6 dhcp option-group to create a static DHCPv6 option group and enter its view.
Use undo ipv6 dhcp option-group to delete the specified static DHCPv6 option group.
ipv6 dhcp option-group option-group-number
undo ipv6 dhcp option-group option-group-number
No static DHCPv6 option groups exist.
context-admin
option-group-number: Assigns an ID to the static option group, in the range of 1 to 100.
A static DHCPv6 option group can use the same ID as a dynamic DHCPv6 option group. If a static DHCPv6 option group and a dynamic DHCPv6 option group use the same ID, the static one takes precedence over the dynamic one.
# Create static DHCPv6 option group 1 and enter its view.
[Sysname] ipv6 dhcp option-group 1
[Sysname-dhcp6-option-group-1]
ipv6 dhcp policy
Use ipv6 dhcp policy to create a DHCPv6 policy and enter its view, or enter the view of an existing DHCPv6 policy.
Use undo ipv6 dhcp policy to delete a DHCPv6 policy.
ipv6 dhcp policy policy-name
undo ipv6 dhcp policy policy-name
No DHCPv6 policies exist.
context-admin
policy-name: Assigns a name to the DHCPv6 policy. The policy name is a case-insensitive string of 1 to 63 characters.
In DHCP policy view, you can specify address pools for different user classes. Clients matching a user class will obtain IPv6 addresses and other parameters from the specified address pool.
For a DHCPv6 policy to take effect, you must apply it to an interface.
# Create DHCPv6 policy test and enter its view.
[Sysname] ipv6 dhcp policy test
[Sysname-dhcp6-policy-test]
class pool
default pool
ipv6 dhcp class
ipv6 dhcp pool
Use ipv6 dhcp pool to create a DHCPv6 address pool and enter its view, or enter the view of an existing DHCPv6 address pool.
Use undo ipv6 dhcp pool to delete the specified DHCPv6 address pool.
ipv6 dhcp pool pool-name
undo ipv6 dhcp pool pool-name
No DHCPv6 address pools exist.
context-admin
pool-name: Specifies a name for the DHCPv6 address pool, a case-insensitive string of 1 to 63 characters.
A DHCPv6 address pool stores IPv6 address/prefix and other configuration parameters to be assigned to DHCPv6 clients.
When you delete a DHCPv6 address pool, binding information for the assigned IPv6 addresses and prefixes in the address pool is also deleted.
# Create a DHCPv6 address pool named pool1 and enter its view.
[Sysname] ipv6 dhcp pool pool1
[Sysname-dhcp6-pool-pool1]
class pool
Use ipv6 dhcp prefix-pool to create a prefix pool and specify the prefix and the assigned prefix length for the pool.
Use undo ipv6 dhcp prefix-pool to delete the specified prefix pool.
ipv6 dhcp prefix-pool prefix-pool-number prefix { prefix-number | prefix/prefix-len } assign-len assign-len [ vpn-instance vpn-instance-name ]
undo ipv6 dhcp prefix-pool prefix-pool-number [ vpn-instance vpn-instance-name ]
No prefix pools exist.
context-admin
prefix-pool-number: Specifies a prefix pool number in the range of 1 to 128.
prefix { prefix-number | prefix/prefix-len }: Specifies a prefix by its ID or in the format of prefix/prefix length. The value range for the prefix-number argument is 1 to 1024. The value range for the prefix-len argument is 1 to 128.
assign-len assign-len: Specifies the assigned prefix length. The value range is 1 to 128, and the value must be greater than or equal to prefix-len. The difference between assign-len and prefix-len must be no more than 16.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. To create a prefix pool for the public network, do not specify this option.
Different prefix pools cannot overlap.
To modify a prefix pool, execute the undo ipv6 dhcp prefix-pool command to delete the prefix pool, and then execute the ipv6 dhcp prefix-pool command.
Deleting a prefix pool clears all prefix bindings from the prefix pool.
When you specify a prefix by its ID, follow these restrictions and guidelines:
·     This command does not take effect if the prefix does not exist. This command takes effect after the prefix is created.
·     Do not specify the same prefix for different prefix pools in a VPN.
·     If the prefix that the ID represents is changed, the prefix range in the prefix pool accordingly changes.
# Create IPv6 prefix 88:99::/32 with ID 3. Configure prefix pool 2 with IPv6 prefix 3 and an assigned prefix length of 42. Prefix pool 2 contains 1024 prefixes from 88:99::/42 to 88:99:FFC0::/42.
[Sysname] ipv6 prefix 3 88:99::/32
[Sysname] ipv6 dhcp prefix-pool 2 prefix 3 assign-len 42
# Create prefix pool 1, and specify prefix 2001:0410::/32 with an assigned prefix length of 42. Prefix pool 1 contains 1024 prefixes from 2001:0410::/42 to 2001:0410:FFC0::/42.
[Sysname] ipv6 dhcp prefix-pool 1 prefix 2001:0410::/32 assign-len 42
prefix-pool
ipv6 dhcp server
Use ipv6 dhcp server to configure global address assignment on an interface. The server on the interface uses a global address pool to assign configuration information to a client.
Use undo ipv6 dhcp server to restore the default.
ipv6 dhcp server { allow-hint | preference preference-value | rapid-commit } *
The server does not support desired address/prefix assignment or rapid address/prefix assignment. The server preference is not set.
Interface view
context-admin
allow-hint: Enables desired address/prefix assignment.
preference preference-value: Specifies the server preference in Advertise messages, in the range of 0 to 255. A greater value represents a higher preference.
rapid-commit: Enables rapid address/prefix assignment involving two messages.
The allow-hint keyword enables the server to assign the desired address or prefix to the requesting client. If the desired address or prefix is not included in any global address pool, or is already assigned to another client, the server assigns the client a free address or a prefix. If the allow-hint keyword is not specified, the server ignores the desired address or prefix, and selects an address or prefix from a global address pool.
If you use the ipv6 dhcp server and ipv6 dhcp server apply pool commands on the same interface, the ipv6 dhcp server apply pool command takes effect.
# Configure global address assignment on the interface GigabitEthernet 1/0/1. Use the desired address/prefix assignment and rapid address/prefix assignment, and set the server preference to the highest 255.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp server allow-hint preference 255 rapid-commit
ipv6 dhcp select
Use ipv6 dhcp server apply pool to apply a DHCPv6 address pool to an interface.
Use undo ipv6 dhcp server apply pool to restore the default.
ipv6 dhcp server apply pool pool-name [ allow-hint | preference preference-value | rapid-commit ] *
No DHCPv6 address pool is applied to an interface.
Interface view
context-admin
preference preference-value: Specifies the server preference in Advertise messages, in the range of 0 to 255. A greater value represents a higher preference. By default, the server preference is not set.
Upon receiving a DHCPv6 request, the DHCPv6 server selects an IPv6 address or prefix from the address pool applied to the receiving interface. If no address pool is applied, the server selects an IPv6 address or prefix from a global address pool that matches the IPv6 address of the receiving interface or the DHCPv6 relay agent.
The allow-hint keyword enables the server to assign the desired address or prefix to the client. If the desired address or prefix does not exist or is already assigned to another client, the server assigns a free address or prefix. If allow-hint is not specified, the server ignores the desired address or prefix, and assigns a free address or prefix.
Only one address pool can be applied to an interface. If you execute this command multiple times, the most recent configuration takes effect.
A non-existing address pool can be applied to an interface, but the server cannot assign any prefix, address, or other configuration information from the address pool until the address pool is created.
# Apply address pool 1 to GigabitEthernet 1/0/1, configure the address pool to support desired address/prefix assignment and address/prefix rapid assignment, and set the preference to 255.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp server apply pool 1 allow-hint preference 255 rapid-commit
ipv6 dhcp pool
ipv6 dhcp select
Use ipv6 dhcp server database filename to configure the DHCPv6 server to back up the DHCPv6 bindings to a file.
Use undo ipv6 dhcp server database filename to restore the default.
ipv6 dhcp server database filename { filename | url url [ username username [ password { cipher | simple } string ] ] }
The DHCPv6 server does not back up the DHCPv6 bindings.
context-admin
filename: Specifies the name of a local backup file. For information about the filename argument, see Fundamentals Configuration Guide.
url url: Specifies the URL of a remote backup file. The URL is a case-sensitive string of 1 to 255 characters. Do not include a username or password in the URL.
username username: Specifies the username for accessing the URL of the remote backup file, a case-sensitive string of 1 to 32 characters. Do not specify this option if a username is not required for accessing the URL of the remote backup file.
string: Specifies the password. Its plaintext form is a case-sensitive string of 1 to 32 characters. Its encrypted form is a case-sensitive string of 1 to 73 characters. Do not specify this argument if a password is not required for accessing the URL of the remote backup file.
The command automatically creates the file if you specify a nonexistent file.
With this command executed, the DHCPv6 server backs up its bindings immediately and runs auto backup. The server, by default, waits 300 seconds after a binding change to update the backup file. You can use the ipv6 dhcp server database update interval command to change the waiting time. If no DHCPv6 binding changes, the backup file is not updated.
As a best practice, back up the bindings to a remote file. If you use the local storage medium, the frequent erasing and writing might damage the medium and then cause the DHCPv6 server to malfunction.
When the backup file is on a remote device, follow these restrictions and guidelines to specify the URL, username, and password:
·     If the file is on an FTP server, enter URL in the format of ftp://server address:port/file path, where the port number is optional.
·     If the file is on a TFTP server, enter URL in the format of tftp://server address:port/file path, where the port number is optional.
·     The username and password must be the same as those configured on the FTP server. If the server authenticates only the username, the password can be omitted.
·     If the IP address of the server is an IPv6 address, enclose the address in a pair of brackets, for example, ftp://[1::1]/database.dhcp.
·     You can also specify the DNS domain name for the server address field, for example, ftp://company/database.dhcp.
# Configure the DHCPv6 server to back up its bindings to the file database.dhcp
[Sysname] ipv6 dhcp server database filename database.dhcp
# Configure the DHCPv6 server to back up its bindings to the file database.dhcp in the working directory of the FTP server at 10::1.
[Sysname] ipv6 dhcp server database filename url ftp://[10::1]/database.dhcp username 1 password simple 1
Use ipv6 dhcp server database update interval to set the waiting time for the DHCPv6 server to update the backup file after a DHCPv6 binding change.
Use undo ipv6 dhcp server database update interval to restore the default.
ipv6 dhcp server database update interval interval
The DHCPv6 server waits 300 seconds to update the backup file after a DHCPv6 binding change. If no DHCPv6 binding changes, the backup file is not updated.
context-admin
interval: Sets the waiting time in the range of 60 to 864000 seconds.
When a DHCPv6 binding is created, updated, or removed, the waiting period starts. The DHCPv6 server updates the backup file when the waiting period is reached. All bindings changed during the period will be saved to the backup file.
The waiting time takes effect only after you configure the DHCPv6 binding auto backup by using the ipv6 dhcp server database filename command.
# Set the waiting time to 600 seconds for the DHCPv6 server to update the backup file.
[Sysname] ipv6 dhcp server database update interval 600
Use ipv6 dhcp server database update now to manually save the DHCPv6 bindings to the backup file.
context-admin
Each time this command is executed, the DHCPv6 bindings are saved to the backup file.
For this command to take effect, you must configure the DHCPv6 auto backup by using the ipv6 dhcp server database filename command.
# Manually save the DHCPv6 bindings to the backup file.
[Sysname] ipv6 dhcp server database update now
Use ipv6 dhcp server database update stop to terminate the download of DHCPv6 bindings from the backup file.
context-admin
The DHCPv6 server does not provide services during the binding download process. If the connection breaks up during the process, the waiting timeout timer is 60 minutes. When the timer expires, the DHCPv6 server stops waiting and starts providing address allocation services. You can execute this command to terminate the download immediately.
Manual termination allows the DHCPv6 server to provide services without waiting for the connection to be repaired. The IPv6 addresses and prefixes associated with the undownloaded bindings will be assigned to clients and address conflicts might occur.
# Terminate the download of the backup DHCPv6 bindings.
[Sysname] ipv6 dhcp server database update stop
Use ipv6 dhcp server forbidden-address to exclude IPv6 addresses in the DHCPv6 address pool from dynamic allocation.
Use undo ipv6 dhcp server forbidden-address to remove the configuration.
ipv6 dhcp server forbidden-address start-ipv6-address [ end-ipv6-address ] [ vpn-instance vpn-instance-name ]
undo ipv6 dhcp server forbidden-address start-ipv6-address [ end-ipv6-address ] [ vpn-instance vpn-instance-name ]
Except for the DHCPv6 server address, all IPv6 addresses in a DHCPv6 address pool are assignable.
context-admin
end-ipv6-address: Specifies the end IPv6 address, which cannot be lower than start-ipv6-address. If you do not specify an end IPv6 address, only the start IPv6 address is excluded from dynamic allocation. If you specify an end IPv6 address, the IP addresses from start-ipv6-address through end-ipv6-address are all excluded from dynamic allocation.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If the excluded IPv6 addresses belong to the public network, do not specify this option.
The IPv6 addresses of some devices such as the gateway and FTP server cannot be assigned to clients. Use this command to exclude such addresses from dynamic allocation.
If the excluded IPv6 address is in a static DHCPv6 binding, the address can still be assigned to the client.
The address or address range specified in the undo form of the command must be the same as the address or address range specified in the command. To remove an IP address that has been specified as part of an address range, you must remove the entire address range.
You can execute this command multiple times to exclude multiple IPv6 address ranges from dynamic allocation.
# Exclude IPv6 addresses of 2001:10:110::1 through 2001:10:110::20 from dynamic assignment.
[Sysname] ipv6 dhcp server forbidden-address 2001:10:110::1 2001:10:110::20
static-bind
Use ipv6 dhcp server forbidden-prefix to exclude IPv6 prefixes in the DHCPv6 prefix pool from dynamic allocation.
Use undo ipv6 dhcp server forbidden-prefix to remove the configuration.
ipv6 dhcp server forbidden-prefix start-prefix/prefix-len [ end-prefix/prefix-len ] [ vpn-instance vpn-instance-name ]
undo ipv6 dhcp server forbidden-prefix start-prefix/prefix-len [ end-prefix/prefix-len ] [ vpn-instance vpn-instance-name ]
No IPv6 prefixes in the DHCPv6 prefix pool are excluded from dynamic allocation.
context-admin
start-prefix/prefix-len: Specifies the start IPv6 prefix. The prefix-len argument specifies the prefix length in the range of 1 to 128.
end-prefix/prefix-len: Specifies the end IPv6 prefix. The prefix-len argument specifies the prefix length in the range of 1 to 128. The value for end-prefix cannot be lower than that for start-prefix. If you do not specify this argument, only the start-prefix/prefix-len is excluded from dynamic allocation. If you specify this argument, the prefixes from start-prefix/prefix-len to end-prefix/prefix-len are all excluded.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If the excluded IPv6 prefixes belong to the public network, do not specify this option.
If the excluded IPv6 prefix is in a static binding, the prefix can still be assigned to the client.
The prefix or prefix range specified in the undo form of the command must be the same as the prefix or prefix range specified in the command. To remove a prefix that has been specified as part of a prefix range, you must remove the entire prefix range.
You can execute this command multiple times to exclude multiple IPv6 prefix ranges from dynamic allocation.
# Exclude IPv6 prefixes from 2001:3e11::/32 through 2001:3eff::/32 from dynamic allocation.
[Sysname] ipv6 dhcp server forbidden-prefix 2001:3e11::/32 2001:3eff::/32
static-bind
network
Use network to specify an IPv6 subnet for dynamic allocation in a DHCPv6 address pool.
Use undo network to restore the default.
network { prefix/prefix-length | prefix prefix-number [ sub-prefix/sub-prefix-length ] } [ preferred-lifetime preferred-lifetime valid-lifetime valid-lifetime ] [ export-route ]
undo network
No IPv6 subnet is specified in a DHCPv6 address pool.
context-admin
prefix/prefix-length: Specifies the IPv6 subnet for dynamic allocation. The value range for the prefix-length argument is 1 to 128.
prefix prefix-number: Specifies an IPv6 prefix by its ID in the range of 1 to 1024.
sub-prefix/sub-prefix-length: Specifies an IPv6 sub-prefix and its length. The value range for the sub-prefix-length argument is 1 to 128. If the IPv6 prefix is longer than the IPv6 sub-prefix or if you do not specify an IPv6 sub-prefix, the IPv6 subnet defined by the IPv6 prefix is used for dynamic allocation.
preferred-lifetime preferred-lifetime: Sets the preferred lifetime. The value range is 60 to 4294967295 seconds, and the default is 604800 seconds (7 days).
valid-lifetime valid-lifetime: Sets the valid lifetime. The value range is 60 to 4294967295 seconds, and the default is 2592000 seconds (30 days). The valid lifetime must be longer than or equal to the preferred lifetime.
export-route: Advertises the subnet assigned to DHCPv6 clients. If you do not specify this keyword, the subnet will not be advertised.
You can specify only one subnet for a DHCPv6 address pool. If you execute the network command multiple times, the most recent configuration takes effect.
Modifying or removing the network command configuration removes assigned addresses in the current address pool.
If you execute the network export-route command multiple times, the most recent configuration takes effect.
The network prefix command does not take effect if the specified IPv6 prefix does not exist. This command takes effect after the IPv6 prefix is created.
The network command defines the IPv6 subnet for dynamic allocation through the prefix/prefix-length arguments or the prefix-number [ sub-prefix/sub-prefix-length ] arguments. The IPv6 subnets cannot be the same in different DHCPv6 address pools.
If the prefix that the ID represents is changed, the IPv6 subnet in this command accordingly changes, and the assigned prefix and address bindings are cleared.
# Specify the subnet 3ffe:501:ffff:100::/64 in DHCPv6 address pool 1.
# Create IPv6 prefix 88:99::/32 with the prefix ID 3. Create DHCPv6 address pool 1 and use the IPv6 subnet defined by the IPv6 prefix for dynamic allocation.
[Sysname-dhcp6-pool-1] network prefix 3
# Create IPv6 prefix 88:99::/32 with the prefix ID 3. Create DHCPv6 address pool 1 and use IPv6 subnet 88:99:ffff:100::/64 defined by IPv6 prefix 3 and IPv6 sub-prefix 3ffe:501:ffff:100::/64 for dynamic allocation. The first 32 bits of the IPv6 subnet are determined by IPv6 prefix 3. The bits 33 to 64 of the IPv6 subnet are determined by the IPv6 sub-prefix and its length. The prefix length of the IPv6 subnet is the IPv6 sub-prefix length.
[Sysname-dhcp6-pool-1] network prefix 3 3ffe:501:ffff:100::/64
address range
temporary address range
option
Use option to configure a self-defined DHCPv6 option in a DHCPv6 address pool.
Use undo option to remove a self-defined DHCPv6 option from a DHCPv6 address pool.
option code hex hex-string
undo option code
No self-defined DHCPv6 option is configured in a DHCPv6 address pool.
context-admin
code: Specifies a number for the self-defined option, in the range of 21 to 65535, excluding 25 through 26, 37 through 40, and 43 through 48.
hex hex-string: Specifies the content of the option, a hexadecimal number whose length is an even number in the range of 2 to 256.
The DHCPv6 server fills the self-defined option with the specified hexadecimal number and sends it in a response to the client.
You can self-define options for the following purposes:
·     Add newly released options.
·     Add options for which the vendor defines the contents, for example, Option 43.
·     Add options for which the CLI does not provide a dedicated configuration command like dns-server. For example, you can use the option 31 hex 02000000000000000000000000000001 command to define the NTP server address 200::1 for DHCP clients.
If a DHCPv6 option is specified by both the dedicated command and the option command, the DHCPv6 server preferentially assigns the content specified by the dedicated command. For example, if a DNS server address is specified by the dns-server command and the option 23 command, the server uses the address specified by dns-server command.
If you execute this command multiple times with the same code specified, the most recent configuration takes effect.
# Configure Option 23 that specifies a DNS server address 2001:f3e0::1 in DHCPv6 address pool 1.
[Sysname-dhcp6-pool-1] option 23 hex 2001f3e0000000000000000000000001
dns-server
domain-name
sip-server
option-group
Use option-group to specify a DHCPv6 option group for a DHCPv6 address pool.
Use undo option-group to restore the default.
undo option-group
No DHCPv6 option group is specified for a DHCPv6 address pool.
context-admin
option-group--number: Specifies a DHCPv6 option group by its number in the range of 1 to 100.
# Specify DHCPv6 option group 1 for DHCPv6 address pool 1.
[Sysname-dhcp6-pool-1] option-group 1
prefix-pool
Use prefix-pool to apply a prefix pool to a DHCPv6 address pool, so the DHCPv6 server can dynamically select a prefix from the prefix pool for a client.
Use undo prefix-pool to remove the prefix pool.
prefix-pool prefix-pool-number [ preferred-lifetime preferred-lifetime valid-lifetime valid-lifetime ]
undo prefix-pool prefix-pool-number
No prefix pool is applied to a DHCPv6 address pool.
DHCPv6 address pool view
context-admin
prefix-pool-number: Specifies a prefix pool by its number in the range of 1 to 128.
preferred-lifetime preferred-lifetime: Sets the preferred lifetime in the range of 60 to 4294967295 seconds. The default value is 604800 seconds (7 days).
valid-lifetime valid-lifetime: Sets the valid lifetime in the range of 60 to 4294967295 seconds. The default value is 2592000 seconds (30 days). The valid lifetime must be longer than or equal to the preferred lifetime.
Only one prefix pool can be applied to an address pool.
You can apply a prefix pool that has not been created to an address pool. The setting takes effect after the prefix pool is created.
To modify the prefix pool in a DHCPv6 address pool, execute the undo prefix-pool command to remove the prefix pool, and then execute the prefix-pool command.
# Apply prefix pool 1 to address pool 1, and use the default preferred lifetime and valid lifetime.
[Sysname-dhcp6-pool-1] prefix-pool 1
# Apply prefix pool 2 to address pool 2, and set the preferred lifetime to one day and the valid lifetime to three days.
[Sysname] ipv6 dhcp pool 2
[Sysname-dhcp6-pool-2] prefix-pool 2 preferred-lifetime 86400 valid-lifetime 259200
reset ipv6 dhcp server conflict
Use reset ipv6 dhcp server conflict to clear IPv6 address conflict information.
reset ipv6 dhcp server conflict [ address ipv6-address ] [ vpn-instance vpn-instance-name ]
context-admin
address ipv6-address: Clears conflict information for the specified IPv6 address. If you do not specify an IPv6 address, this command clears all IPv6 address conflict information.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears conflict information about IPv6 addresses for the public network.
Address conflicts occur when dynamically assigned IP addresses have been statically configured for other hosts. After the conflicts are resolved, you can use the reset ipv6 dhcp server conflict command to clear conflict information so that the conflicted addresses can be assigned to clients.
# Clear all IPv6 address conflict information.
<Sysname> reset ipv6 dhcp server conflict
reset ipv6 dhcp server expired
Use reset ipv6 dhcp server expired to clear binding information for lease-expired IPv6 addresses.
reset ipv6 dhcp server expired [ [ address ipv6-address ] [ vpn-instance vpn-instance-name ] | pool pool-name ]
context-admin
address ipv6-address: Clears binding information for the specified lease-expired IPv6 address. If you do not specify an IPv6 address, this command clears binding information for all lease-expired IPv6 address.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears binding information about lease-expired IPv6 addresses for the public network.
pool pool-name: Clears binding information for lease-expired IPv6 addresses in the address pool specified by its name, a case-insensitive string of 1 to 63 characters. If you do not specify an address pool, this command clears binding information for lease-expired IPv6 addresses in all address pools.
# Clear binding information for expired IPv6 address 2001:f3e0::1.
<Sysname> reset ipv6 dhcp server expired address 2001:f3e0::1
reset ipv6 dhcp server ip-in-use
Use reset ipv6 dhcp server ip-in-use to clear binding information for assigned IPv6 addresses.
reset ipv6 dhcp server ip-in-use [ [ address ipv6-address ] [ vpn-instance vpn-instance-name ] | pool pool-name ]
context-admin
address ipv6-address: Clears binding information for the specified assigned IPv6 address. If you do not specify an IPv6 address, this command clears binding information for all assigned IPv6 addresses.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears binding information about assigned IPv6 addresses for the public network.
pool pool-name: Clears binding information for assigned IPv6 addresses in the address pool specified by its name, a case-insensitive string of 1 to 63 characters. If you do not specify an address pool, this command clears binding information for assigned IPv6 addresses in all address pools.
If you execute this command to clear information about an assigned static binding, the static binding becomes a free static binding.
# Clear binding information for all assigned IPv6 addresses.
<Sysname> reset ipv6 dhcp server ip-in-use
# Clears binding information for assigned IPv6 addresses in DHCPv6 address pool 1.
<Sysname> reset ipv6 dhcp server ip-in-use pool 1
# Clears binding information for the assigned IPv6 address 2001:0:0:1::1.
<Sysname> reset ipv6 dhcp server ip-in-use address 2001:0:0:1::1
reset ipv6 dhcp server pd-in-use
Use reset ipv6 dhcp server pd-in-use to clear binding information for assigned IPv6 prefixes.
reset ipv6 dhcp server pd-in-use [ pool pool-name | [ prefix prefix/prefix-len ] [ vpn-instance vpn-instance-name ] ]
context-admin
pool pool-name: Clears binding information for assigned IPv6 prefixes in the address pool specified by its name, a case-insensitive string of 1 to 63 characters. If you do not specify an address pool, this command clears binding information for assigned IPv6 prefixes in all address pools.
prefix prefix/prefix-len: Clears binding information for the specified assigned IPv6 prefix. The value range for the prefix length is 1 to 128. If you do not specify an IPv6 prefix, this command clears binding information for all assigned IPv6 prefixes.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears binding information about assigned IPv6 prefixes for the public network.
# Clear binding information for all assigned IPv6 prefixes.
<Sysname> reset ipv6 dhcp server pd-in-use
# Clears binding information for assigned IPv6 prefixes in DHCPv6 address pool 1.
<Sysname> reset ipv6 dhcp server pd-in-use pool 1
# Clears binding information for the assigned IPv6 prefix 2001:0:0:1::/64.
<Sysname> reset ipv6 dhcp server pd-in-use prefix 2001:0:0:1::/64
reset ipv6 dhcp server statistics
Use reset ipv6 dhcp server statistics to clear DHCPv6 server statistics.
reset ipv6 dhcp server statistics [ vpn-instance vpn-instance-name ]
context-admin
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears DHCPv6 server statistics for the public network.
# Clear DHCPv6 server statistics.
<Sysname> reset ipv6 dhcp server statistics
sip-server
Use sip-server to specify the IPv6 address or domain name of a SIP server in the DHCPv6 address pool.
Use undo sip-server to remove a SIP server.
sip-server { address ipv6-address | domain-name domain-name }
undo sip-server { address ipv6-address | domain-name domain-name }
No SIP server address or domain name is specified.
context-admin
address ipv6-address: Specifies the IPv6 address of a SIP server.
domain-name domain-name: Specifies the domain name of a SIP server, a case-insensitive string of 1 to 50 characters.
You can specify up to eight SIP server addresses and eight SIP server domain names in an address pool. A SIP server that is specified earlier has a higher preference.
# Specify the SIP server address 2:2::4 in DHCPv6 address pool 1.
[Sysname] ipv6 dhcp pool 1
[Sysname-dhcp6-pool-1] sip-server address 2:2::4
# Specify the SIP server domain name bbb.example.com in DHCPv6 address pool 1.
[Sysname-dhcp6-pool-1] sip-server domain-name bbb.example.com
display ipv6 dhcp pool
static-bind
Use static-bind to statically bind an IPv6 address or prefix to a client in the DHCPv6 address pool.
Use undo static-bind to delete a static binding.
static-bind { address ipv6-address/addr-prefix-length | prefix prefix/prefix-len } duid duid [ iaid iaid ] [ preferred-lifetime preferred-lifetime valid-lifetime valid-lifetime ] [ description description-text ]
undo static-bind { address ipv6-address/addr-prefix-length | prefix prefix/prefix-len }
No static binding is configured in a DHCPv6 address pool.
context-admin
address ipv6-address/addr-prefix-length: Specifies the IPv6 address and prefix length. The value range for the prefix length is 1 to 128.
prefix prefix/prefix-len: Specifies the prefix and prefix length. The value range for the prefix length is 1 to 128.
duid duid: Specifies a client DUID. The value is an even hexadecimal number in the range of 2 to 256.
iaid iaid: Specifies a client IAID. The value is a hexadecimal number in the range of 0 to FFFFFFFF. If you do not specify an IAID, the server does not match the client IAID for prefix assignment.
preferred-lifetime preferred-lifetime: Sets the preferred lifetime of the address or prefix. The value range is 60 to 4294967295 seconds, and the default is 604800 seconds (7 days).
valid-lifetime valid-lifetime: Sets the valid lifetime of the address or prefix. The value range is 60 to 4294967295 seconds, and the default is 2592000 seconds (30 days). The valid lifetime cannot be shorter than the preferred lifetime.
description description-text: Specifies a description for the static binding, a case-sensitive string of 1 to 255 characters.
You can specify multiple static bindings in a DHCPv6 address pool.
An IPv6 address or prefix can be bound to only one DHCPv6 client.
To modify a static binding, execute the undo static-bind command to delete the binding, and then execute the static-bind command.
This command is not supported in IPv6 address pools that are configured with the remote-server command and act as DHCPv6 relay address pools.
# In address pool 1, bind IPv6 address 2001:0410::/35 to the client DUID 0003000100e0fc005552 and IAID A1A1A1A1.
[Sysname-dhcp6-pool-1] static-bind address 2001:0410::/35 duid 0003000100e0fc005552 iaid A1A1A1A1
# In address pool 1, bind prefix 2001:0410::/35 to the client DUID 00030001CA0006A400 and IAID A1A1A1A1.
[Sysname-dhcp6-pool-1] static-bind prefix 2001:0410::/35 duid 00030001CA0006A400 iaid A1A1A1A1
Use temporary address range to configure a temporary IPv6 address range in a DHCPv6 address pool for dynamic allocation.
Use undo temporary address range to restore the default.
temporary address range start-ipv6-address end-ipv6-address [ preferred-lifetime preferred-lifetime valid-lifetime valid-lifetime ]
No temporary IPv6 address range is configured in a DHCPv6 address pool.
context-admin
start-ipv6-address: Specifies the start IPv6 address.
end-ipv6-address: Specifies the end IPv6 address.
valid-lifetime valid-lifetime: Sets the valid lifetime. The value range is 60 to 4294967295 seconds, and the default is 2592000 seconds (30 days). The valid lifetime cannot be shorter than the preferred lifetime.
If you do not execute the temporary address range command, the DHCPv6 server does not support temporary address assignment.
You can configure only one temporary IPv6 address range in an address pool. If you execute this command multiple times, the most recent configuration takes effect.
# In DHCPv6 address pool 1, configure a temporary IPv6 address range from 3ffe:501:ffff:100::50 to 3ffe:501:ffff:100::60.
[Sysname-dhcp6-pool-1] network 3ffe:501:ffff:100::/64
[Sysname-dhcp6-pool-1] temporary address range 3ffe:501:ffff:100::50 3ffe:501:ffff:100::60
address range
network
vpn-instance
Use vpn-instance to apply a DHCPv6 address pool to a VPN instance.
Use undo vpn-instance to restore the default.
undo vpn-instance
The DHCPv6 address pool is not applied to any VPN instance.
context-admin
vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, the DHCPv6 address pool belongs to the public network.
If a DHCPv6 address pool is applied to a VPN instance, the DHCPv6 server assigns IPv6 addresses in this address pool to clients in the specified VPN instance.
The DHCPv6 server identifies the VPN instance to which a DHCPv6 client belongs according to the following information:
·     The client's VPN information stored in authentication modules.
·     The VPN information of the DHCPv6 server's interface that receives DHCPv6 packets from the client.
The VPN information from authentication modules takes priority over the VPN information of the receiving interface.
# Apply DHCPv6 address pool 0 to the VPN instance abc.
[Sysname] ipv6 dhcp pool 0
[Sysname-dhcp6-pool-0] vpn-instance abc
DHCPv6 relay agent commands
display ipv6 dhcp relay server-address
Use display ipv6 dhcp relay server-address to display DHCPv6 server addresses specified on a DHCPv6 relay interface.
display ipv6 dhcp relay server-address [ interface interface-type interface-number ]
context-admin
context-operator
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays DHCPv6 server addresses on all interfaces enabled with DHCPv6 relay agent.
# Display DHCPv6 server addresses on all interfaces enabled with DHCPv6 relay agent.
<Sysname> display ipv6 dhcp relay server-address
 Server address                             Outgoing Interface
 2::3
 3::4                                       GigabitEthernet1/0/3
 2::3
# Display DHCPv6 server addresses on GigabitEthernet 1/0/1.
<Sysname> display ipv6 dhcp relay server-address interface gigabitethernet 1/0/1
 2::3
Table 11 Command output
Server address
DHCPv6 server address specified on the DHCP relay agent.
Outgoing Interface
Output interface of DHCPv6 packets. If no output interface is specified, the device searches the routing table for the output interface.
ipv6 dhcp select
display ipv6 dhcp relay statistics
Use display ipv6 dhcp relay statistics to display DHCPv6 packet statistics on the DHCPv6 relay agent.
display ipv6 dhcp relay statistics [ interface interface-type interface-number ]
context-admin
context-operator
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays DHCPv6 packets statistics on all interfaces enabled with DHCPv6 relay agent.
# Display DHCPv6 packet statistics on all interfaces enabled with DHCPv6 relay agent.
<Sysname> display ipv6 dhcp relay statistics
Packets dropped               :  4
Packets received              :  14
    Solicit                   :  0
    Request                   :  0
    Confirm                   :  0
    Renew                     :  0
    Rebind                    :  0
    Release                   :  0
    Decline                   :  0
    Information-request       :  7
    Relay-forward             :  0
    Relay-reply               :  7
Packets sent                  :  14
    Advertise                 :  0
    Reconfigure               :  0
    Reply                     :  7
    Relay-forward             :  7
    Relay-reply               :  0
# Display DHCPv6 packet statistics on the DHCPv6 relay agent on GigabitEthernet 1/0/1.
<Sysname> display ipv6 dhcp relay statistics interface gigabitethernet 1/0/1
Packets dropped               :  4
Packets received              :  16
    Solicit                   :  0
    Request                   :  0
    Confirm                   :  0
    Renew                     :  0
    Rebind                    :  0
    Release                   :  0
    Decline                   :  0
    Information-request       :  8
    Relay-forward             :  0
    Relay-reply               :  8
Packets sent                  :  16
    Advertise                 :  0
    Reconfigure               :  0
    Reply                     :  8
    Relay-forward             :  8
    Relay-reply               :  0
Table 12 Command output
Packets dropped
Number of discarded packets.
Packets received
Number of received packets.
Solicit
Number of received solicit packets.
Request
Number of received request packets.
Confirm
Number of received confirm packets.
Renew
Number of received renew packets.
Rebind
Number of received rebind packets.
Release
Number of received release packets.
Decline
Number of received decline packets.
Information-request
Number of received information request packets.
Relay-forward
Number of received relay-forward packets.
Relay-reply
Number of received relay-reply packets.
Packets sent
Number of sent packets.
Advertise
Number of sent advertise packets.
Reconfigure
Number of sent reconfigure packets.
Reply
Number of sent reply packets.
Relay-forward
Number of sent Relay-forward packets.
Relay-reply
Number of sent Relay-reply packets.
reset ipv6 dhcp relay statistics
gateway-list
Use gateway-list to specify gateway addresses for DHCPv6 clients in a DHCPv6 address pool.
Use undo gateway-list to remove gateway addresses from a DHCPv6 address pool.
gateway-list ipv6-address&<1-8>
undo gateway-list [ ipv6-address&<1-8> ]
No gateway address is specified in a DHCPv6 address pool.
context-admin
ipv6-address&<1-8>: Specifies a space-separated list of up to eight addresses.
DHCPv6 clients of the same access type can be classified into different types by their locations. In this case, the relay interface typically has no IPv6 address configured. You can use the gateway-list command to specify gateway addresses for clients matching the same DHCPv6 address pool.
Upon receiving a DHCPv6 Solicit or Request from a client that matches a DHCPv6 address pool, the relay agent processes the packet as follows:
·     Fills the link-address field of the packet with a specified gateway address.
·     Forwards the packet to all DHCPv6 servers in the matching DHCPv6 address pool.
The DHCPv6 servers select a DHCPv6 address pool according to the gateway address.
# Specify the gateway address 10::1 in the DHCPv6 address pool p1.
[Sysname] ipv6 dhcp pool p1
[Sysname-dhcp6-pool-p1] gateway-list 10::1
ipv6 dhcp relay client-link-address enable
Use ipv6 dhcp relay client-link-address enable to enable the DHCPv6 relay agent to support Option 79.
Use undo ipv6 dhcp relay client-link-address enable to disable Option 79 support.
The DHCPv6 relay agent does not support Option 79.
Interface view
context-admin
If DHCPv6 relay agents exist in the network, the DHCPv6 server needs the MAC address of the DHCPv6 client for authentication or for IPv6 address or prefix assignment. To meet the requirement, enable the DHCPv6 relay agent that the client's DHCPv6 requests first pass to support Option 79. This feature allows the DHCPv6 relay agent to learn the MAC address in the client request. When the relay agent generates a Relay-Forward packet for the request, it inserts the MAC address of the client into Option 79. The Relay-Forward packet is then forwarded to the DHCPv6 server.
# Enable Option 79 support on the relay agent.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp relay client-link-address enable
ipv6 dhcp relay gateway
Use ipv6 dhcp relay gateway to specify a gateway address for DHCPv6 clients on the DHCPv6 relay interface.
Use undo ipv6 dhcp relay gateway to restore the default.
ipv6 dhcp relay gateway ipv6-address
The first IPv6 address of the relay interface is used as the gateway address for DHCPv6 clients.
Interface view
context-admin
ipv6-address: Specifies a gateway address. The IPv6 address must be an IPv6 address of the relay interface.
The DHCPv6 relay agent uses the specified IPv6 address instead of the first IPv6 address of the relay interface as the gateway address for DHCPv6 clients.
# Specify 10::1 as the gateway address for DHCPv6 clients on GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp relay gateway 10::1
gateway-list
ipv6 dhcp relay interface-id
Use ipv6 dhcp relay interface-id to specify a padding mode for the Interface-ID option.
Use undo ipv6 dhcp relay interface-id to restore the default.
ipv6 dhcp relay interface-id { bas | interface }
The DHCPv6 relay agent fills the Interface-ID option with the interface index of the interface.
Interface view
context-admin
bas: Specifies the BAS mode.
interface: Specifies the interface name mode. This mode pads the Interface-ID option in ASCII code with the interface name and VLAN ID of the interface.
Enable the DHCPv6 relay agent on the interface before executing this command. Otherwise, the command does not take effect.
# Specify the BAS mode as the padding mode for the Interface-ID option on GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp relay interface-id bas
# Specify the interface name mode as the padding mode for the Interface-ID option on GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp relay interface-id interface
Use ipv6 dhcp relay server-address to specify a DHCPv6 server on the DHCPv6 relay agent.
Use undo ipv6 dhcp relay server-address to remove DHCPv6 server addresses.
ipv6 dhcp relay server-address ipv6-address [ interface interface-type interface-number ]
undo ipv6 dhcp relay server-address [ ipv6-address [ interface interface-type interface-number ] ]
No DHCPv6 server address is specified on the DHCPv6 relay agent.
Interface view
context-admin
ipv6-address: Specifies the IPv6 address of a DHCPv6 server.
interface interface-type interface-number: Specifies an output interface through which the relay agent forwards the DHCPv6 requests to the DHCPv6 server. If you do not specify an output interface, the relay agent looks up the routing table for an output interface.
Upon receiving a request from a DHCPv6 client, the interface encapsulates the request into a Relay-forward message and forwards the message to the specified DHCPv6 server.
You can specify a maximum of eight DHCPv6 servers on an interface. The DHCPv6 relay agent forwards DHCP requests to all the specified DHCPv6 servers.
If the DHCPv6 server address is a link-local address or multicast address, you must specify an output interface. If you do not specify an output interface, DHCPv6 packets might fail to reach the DHCPv6 server.
If you do not specify an IPv6 address, the undo ipv6 dhcp relay server-address command removes all DHCPv6 server addresses specified on the interface.
Do not enable the DHCPv6 client and the DHCPv6 relay agent on the same interface.
# Enable the DHCPv6 relay agent on GigabitEthernet 1/0/1 and specify the DHCPv6 server address 2001:1::3.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp select relay
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp relay server-address 2001:1::3
ipv6 dhcp select
remote-server
Use remote-server to specify DHCPv6 servers for a DHCPv6 address pool.
Use undo remote-server to remove DHCPv6 servers from a DHCPv6 address pool.
remote-server ipv6-address [ interface interface-type interface-number ]
undo remote-server [ ipv6-address [ interface interface-type interface-number ] ]
No DHCPv6 server is specified for the DHCPv6 address pool.
context-admin
ipv6-address: Specifies a DHCPv6 server address.
interface interface-type interface-number: Specifies the outgoing interface by its type and number for the DHCPv6 relay agent to forward packets to the DHCPv6 server. If you do not specify an outgoing interface, the DHCPv6 relay agent performs a routing table lookup.
You can specify a maximum of eight DHCPv6 servers in one DHCPv6 address pool.
If you do not specify any parameters, the undo remote-server command removes all DHCPv6 servers in the DHCPv6 address pool.
If a DHCPv6 server address is a link-local address, you must specify an outgoing interface by using the interface keyword in this command. If you do not specify an outgoing interface, DHCPv6 packets might fail to reach the DHCPv6 server.
# Specify DHCPv6 server 10::1 for DHCPv6 address pool 0.
[Sysname-dhcp6-pool-0] remote-server 10::1
Use reset ipv6 dhcp relay statistics to clear packets statistics on the DHCPv6 relay agent.
reset ipv6 dhcp relay statistics [ interface interface-type interface-number ]
context-admin
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command clears all relay agent statistics.
# Clear packet statistics on the DHCPv6 relay agent.
<Sysname> reset ipv6 dhcp relay statistics
DHCPv6 client commands
display ipv6 dhcp client
Use display ipv6 dhcp client to display DHCPv6 client information.
display ipv6 dhcp client [ interface interface-type interface-number ]
context-admin
context-operator
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays information about all DHCPv6 clients.
# Display the DHCPv6 client information on GigabitEthernet 1/0/1.
<Sysname> display ipv6 dhcp client interface gigabitethernet 1/0/1
GigabitEthernet1/0/1:
  Type: Stateful client requesting address and prefix
    State: OPEN
    Client DUID: 0003000100e002000000
    Preferred server
      Reachable via address: FE80::2E0:1FF:FE00:18
      Server DUID: 0003000100e001000000
    IA_NA: IAID 0x00000642, T1 50 sec, T2 80 sec
      Address: 1:1::2/128
        Preferred lifetime 100 sec, valid lifetime 200 sec
        Will expire on Feb 4 2014 at 15:37:20(288 seconds left)
    IA_PD: IAID 0x00000642, T1 50 sec, T2 80 sec
      Prefix: 12:34::/48
        Will expire on Mar 27 2014 at 08:13:24 (199 seconds left)
    DNS server addresses:
      2:2::3
    Domain name:
      aaa.example.com
    SIP server addresses:
      2:2::4
    SIP server domain names:
      bbb.example.com
    Options:
      Code: 88
        Length: 3 bytes
        Hex: AABBCC
Table 13 Command output
Types of DHCPv6 client:
·     Stateful client requesting address—A DHCPv6 client that requests an IPv6 address.
·     Stateful client requesting prefix—A DHCPv6 client that requests an IPv6 prefix.
·     Stateful client requesting address and prefix—A DHCPv6 client that requests an IPv6 address and prefix.
·     Stateless client—A DHCPv6 client that requests configuration parameters other than an IPv6 address and prefix through stateless DHCPv6.
Current state of the DHCPv6 client:
·     IDLE—The client is in idle state.
·     SOLICIT—The client is locating a DHCPv6 server.
·     REQUEST—The client is requesting an IPv6 address or prefix.
·     OPEN—The client has obtained an IPv6 address or prefix.
·     RENEW—The client is extending the lease (after T1 and before T2).
·     REBIND—The client is extending the lease (after T2 and before the lease expires).
·     RELEASE—The client is releasing an IPv6 address or prefix.
·     DECLINE—The client is declining an IPv6 address or prefix because of an address or prefix conflict.
·     INFO-REQUESTING—The client is requesting configuration parameters through stateless DHCPv6.
Client DUID
DUID of the DHCPv6 client.
Preferred server
Information about the DHCPv6 server selected by the DHCPv6 client.
Reachable address for the DHCPv6 client. It is the link local address of the DHCPv6 server or DHCPv6 relay agent.
Server DUID
DUID of the DHCPv6 server.
IA_NA
IA_NA information.
IA_PD
IA_PD information.
IAID
IA identifier.
T1
T1 value in seconds.
T2
T2 value in seconds.
Address
IPv6 address obtained. This field is displayed only when the DHCPv6 client type is Stateful client requesting address.
Prefix
IPv6 prefix obtained. This field is displayed only when the DHCPv6 client type is Stateful client requesting prefix.
Preferred lifetime
Preferred lifetime in seconds.
valid lifetime
Valid lifetime in seconds.
Will expire on Feb 4 2014 at 15:37:20 (288 seconds left)
Time when the lease expires and the remaining time of the lease.
If the lease expires after the year 2100, this field displays Will expire after 2100.
IPv6 address of the DNS server.
Domain name
Domain name suffix.
IPv6 address of the SIP server.
Domain name of the SIP server.
Options
Self-defined options.
Code
Code of the self-defined option.
Length
Self-defined option length in bytes.
Hex
Self-defined option content represented by a hexadecimal number.
ipv6 address dhcp-alloc
ipv6 dhcp client duid
ipv6 dhcp client pd
display ipv6 dhcp client statistics
Use display ipv6 dhcp client statistics to display DHCPv6 client statistics.
display ipv6 dhcp client statistics [ interface interface-type interface-number ]
context-admin
context-operator
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays statistics for all DHCPv6 clients.
# Display DHCPv6 client statistics on GigabitEthernet 1/0/1.
<Sysname> display ipv6 dhcp client statistics interface gigabitethernet 1/0/1
Interface                     :  GigabitEthernet1/0/1
         Reply                :  1
         Advertise            :  0
         Reconfigure         :   0
         Invalid              :  0
Packets sent                  :  5
         Solicit              :  0
         Request              :  0
         Renew                :  0
         Rebind               :  0
         Information-request  :  5
         Release              :  0
         Decline              :  0
Table 14 Command output
Interface that acts as the DHCPv6 client.
Packets Received
Reply
Number of received reply packets.
Advertise
Number of received advertise packets.
Reconfigure
Number of received reconfigure packets.
Invalid
Number of invalid packets.
Packets sent
Solicit
Number of sent solicit packets.
Request
Number of sent request packets.
Renew
Number of sent renew packets.
Rebind
Number of sent rebind packets.
Information-request
Number of sent information request packets.
Release
Number of sent release packets.
Decline
Number of sent decline packets.
reset ipv6 dhcp client statistics
Use ipv6 address dhcp-alloc to configure an interface to use DHCPv6 for IPv6 address acquisition.
Use undo ipv6 address dhcp-alloc to cancel an interface from using DHCPv6, and clear the obtained IPv6 address and other configuration parameters.
ipv6 address dhcp-alloc [ option-group option-group-number | rapid-commit ] *
An interface does not use DHCPv6 for IPv6 address acquisition.
VLAN interface view
Reth interface view
Reth subinterface view
context-admin
option-group option-group-number: Enables the DHCPv6 client to create a dynamic DHCPv6 option group for saving the configuration parameters, and assigns an ID to the option group. The value range for the ID is 1 to 100. If you do not specify this option, the DHCPv6 client does not create any dynamic DHCPv6 option groups.
rapid-commit: Supports rapid address or prefix assignment.
# Configure GigabitEthernet 1/0/1 to use DHCPv6 for IPv6 address acquisition. Configure the DHCPv6 client to support rapid address assignment and create dynamic DHCPv6 option group 1 for the configuration parameters obtained.
[Sysname-GigabitEthernet1/0/1] ipv6 address dhcp-alloc rapid-commit option-group 1
ipv6 dhcp client dscp
Use ipv6 dhcp client dscp to set the DSCP value for DHCPv6 packets sent by the DHCPv6 client.
Use undo ipv6 dhcp client dscp to restore the default.
ipv6 dhcp client dscp dscp-value
The DSCP value in DHCPv6 packets is 56.
context-admin
dscp-value: Sets the DSCP value for DHCP packets, in the range of 0 to 63.
The DSCP value is carried in the Traffic class field of a DHCPv6 packet. It specifies the priority level of the packet and affects the transmission priority of the packet. A bigger DSCP value represents a higher priority.
# Set the DSCP value to 30 for DHCPv6 packets sent by the DHCPv6 client.
[Sysname] ipv6 dhcp client dscp 30
Use ipv6 dhcp client duid to configure the DHCPv6 client DUID for an interface.
Use undo ipv6 dhcp client duid to restore the default.
ipv6 dhcp client duid { ascii ascii-string | hex hex-string | mac interface-type interface-number }
The interface uses the device bridge MAC address to generate its DHCPv6 client DUID.
VLAN interface view
Reth interface view
context-admin
ascii ascii-string: Specifies a case-sensitive ASCII string of 1 to 130 characters as the DHCPv6 client DUID.
hex hex-string: Specifies a hexadecimal number of 2 to 260 characters as the DHCPv6 client DUID.
mac interface-type interface-number: Specifies the MAC address of the specified interface as the DHCPv6 client DUID. The interface-type interface-number arguments specify an interface by its type and number.
A DHCPv6 client pads its DUID into the Option 1 of the DHCPv6 packet that it sends to the DHCPv6 server. The DHCPv6 server can assign specific IPv6 addresses or prefixes to DHCPv6 clients with specific DUIDs.
The DUID of a DHCPv6 client is the globally unique identifier of the client, so make sure the DUID that you configure is unique.
# Specify the MAC address of GigabitEthernet 1/0/2 as the DHCPv6 client DUID for GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp client duid mac gigabitethernet 1/0/2
ipv6 dhcp client pd
Use ipv6 dhcp client pd to configure an interface to use DHCPv6 for IPv6 prefix acquisition.
Use undo ipv6 dhcp client pd to cancel an interface from using DHCPv6, and clear the obtained IPv6 prefix and other configuration parameters.
ipv6 dhcp client pd prefix-number [ option-group option-group-number | rapid-commit ]*
An interface does not use DHCPv6 for IPv6 prefix acquisition.
VLAN interface view
Reth interface view
context-admin
prefix-number: Specifies an IPv6 prefix ID in the range of 1 to 1024. After obtaining an IPv6 prefix, the client assigns the ID to the IPv6 prefix.
# Configure GigabitEthernet 1/0/1 to use DHCPv6 for IPv6 prefix acquisition. Specify IDs for the dynamic IPv6 prefix and dynamic DHCPv6 option group, and configure the client to support rapid prefix assignment.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp client pd 1 rapid-commit option-group 1
ipv6 dhcp client stateful
Use ipv6 dhcp client stateful to configure an interface to use DHCPv6 for IPv6 address and prefix acquisition.
Use undo ipv6 dhcp client stateful to cancel an interface from using DHCPv6, and clear the obtained IPv6 address, prefix, and other configuration parameters.
ipv6 dhcp client stateful prefix prefix-number [ option-group option-group-number | rapid-commit ] *
An interface does not use DHCPv6 for IPv6 address and prefix acquisition.
VLAN interface view
Reth interface view
context-admin
prefix prefix-number: Specifies an IPv6 prefix ID in the range of 1 to 1024. After obtaining an IPv6 prefix, the client assigns the ID to the IPv6 prefix.
rapid-commit: Supports rapid address and prefix assignment.
The ipv6 dhcp client stateful command takes effect if it is configured with the ipv6 address dhcp-alloc and ipv6 dhcp client pd commands on an interface. You must execute the undo ipv6 dhcp client stateful command to have the ipv6 address dhcp-alloc and ipv6 dhcp client pd commands take effect.
# Configure GigabitEthernet 1/0/1 to use DHCPv6 for IPv6 address and prefix acquisition. Specify IDs for the dynamic IPv6 prefix and dynamic DHCPv6 option group, and configure the client to support rapid address and prefix assignment.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp client stateful prefix 1 rapid-commit option-group 1
ipv6 dhcp client pd
ipv6 dhcp client stateless enable
Use ipv6 dhcp client stateless enable to enable stateless DHCPv6.
Use undo ipv6 dhcp client stateless enable to disable stateless DHCPv6.
Stateless DHCPv6 is disabled.
VLAN interface view
Reth interface view
context-admin
Stateless DHCPv6 enables the interface to send an Information-request message to the multicast address of all DHCPv6 servers and DHCPv6 relay agents for configuration parameters.
# Enable stateless DHCPv6 on GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] ipv6 dhcp client stateless enable
Use reset ipv6 dhcp client statistics to clear DHCPv6 client statistics.
reset ipv6 dhcp client statistics [ interface interface-type interface-number ]
context-admin
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command clears all DHCPv6 client statistics.
# Clear all DHCPv6 client statistics.
<Sysname> reset ipv6 dhcp client statistics