20-Network Management and Monitoring
HomeSupportRoutersCR16000-F SeriesReference GuidesMIB CompanionH3C CR16000-F Routers MIB Reference-R838x-6W10020-Network Management and Monitoring
12-HH3C-TWAMP-MIB
12-HH3C-TWAMP-MIB 152.59 KB
HH3C-TWAMP-MIB
About this MIB
Use HH3C-TWAMP-MIB to implement NQA TWAMP Light as follows:
Enable the TWAMP Light client and the TWAMP Light sender.
Configure and obtain information about test sessions on the TWAMP Light client.
Configure and obtain packet sending intervals, timeout time of the reflected packet, and statistics collection interval for TWAMP Light tests on the TWAMP Light sender.
Obtain the TWAMP Light sender status.
Obtain two-way delay and two-way jitter statistics for TWAMP Light tests on the TWAMP Light sender.
Obtain two-way packet loss statistics for TWAMP Light tests on the TWAMP Light sender.
Obtain the largest index value in TWAMP loss results and TWAMP delay results.
Clear statistics about TWAMP Light tests.
Enable the TWAMP Light responder.
Configure and obtain information about test sessions on the TWAMP Light responder.
MIB file name
hh3c-twamp.mib
Root object
iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).hh3c(25506).hh3cCommon(2).hh3cTwamp(184)
Scalar objects
hh3cTwamplightSenderEnable (1.3.6.1.4.1.25506.2.184.2.1.2)
Object (OID)
Access
Value range
Implementation
read-write
TruthValue
Standard MIB values.
Enabling status of the TWAMP Light sender.
As per the MIB.
hh3cTwamplightRespondeEnable(1.3.6.1.4.1.25506.2.184.2.2.1)
Object (OID)
Access
Value range
Implementation
read- write
TruthValue
Enabling status of the TWAMP Light responder.
As per the MIB.
Tabular objects
hh3cTwamplightClientTable
About this table
Use this table to configure and obtain information about test sessions on the TWAMP Light client.
Support for operations
CreateSupported
Edit/ModifySupported
DeleteSupported
ReadSupported
Columns
The table index is hh3cTwamplightControllerID.
Object (OID)
Access
Value range
Implementation
hh3cTwamplightControllerID(1.3.6.1.4.1.25506.2.184.2.1.3.1.1)
accessible-for-notify
Integer32
Integer32(1..512)
Test session ID.
Implementation varies by product.
hh3cTwamplightClientSrcAddrType(1.3.6.1.4.1.25506.2.184.2.1.3.1.2)
read-create
InetAddressType
Type of the source address.
As per the MIB.
hh3cTwamplightClientSrcAddr(1.3.6.1.4.1.25506.2.184.2.1.3.1.3)
read-create
InetAddress
Source IP address.
As per the MIB.
hh3cTwamplightClientTrgtAddrType(1.3.6.1.4.1.25506.2.184.2.1.3.1.4)
read-create
InetAddressType
Type of the destination IP address.
As per the MIB.
hh3cTwamplightClientTrgtAddr(1.3.6.1.4.1.25506.2.184.2.1.3.1.5)
read-create
InetAddress
Destination IP address.
As per the MIB.
hh3cTwamplightClientSrcPort(1.3.6.1.4.1.25506.2.184.2.1.3.1.6)
read-create
Integer32
Integer32(0..65535)
Source port number.
As per the MIB.
hh3cTwamplightClientTrgtPort(1.3.6.1.4.1.25506.2.184.2.1.3.1.7)
read-create
Integer32
Integer32(0..65535)
Destination port number.
As per the MIB.
hh3cTwamplightClientVPN(1.3.6.1.4.1.25506.2.184.2.1.3.1.8)
read-create
DisplayString
OCTET STRING(0..31)
MPLS L3VPN instance name.
As per the MIB.
hh3cTwamplightClientDscp
(1.3.6.1.4.1.25506.2.184.2.1.3.1.9)
read-create
Integer32
integer32(0..63)
Differentiated services code point (DSCP) value.
As per the MIB.
hh3cTwamplightClientDataSize(1.3.6.1.4.1.25506.2.184.2.1.3.1.10)
read-create
Integer32
Integer32(44..1518)
Probe packet size.
As per the MIB.
hh3cTwamplightClientDescription(1.3.6.1.4.1.25506.2.184.2.1.3.1.11)
read-create
DisplayString
OCTET STRING(0..200)
Description for the test session.
As per the MIB.
hh3cTwamplightClientRowStatus(1.3.6.1.4.1.25506.2.184.2.1.3.1.12)
read-create
RowStatus
Manages the creation and deletion of the conceptual row.
Supports only active(1), createAndGo(2), and destroy(6).
hh3cTwamplightClientSrcIfName(1.3.6.1.4.1.25506.2.184.2.1.3.1.13)
read-create
DisplayString
OCTET STRING(0..47)
Source interface type and number.
As per the MIB.
hh3cTwamplightClientServiceID(1.3.6.1.4.1.25506.2.184.2.1.3.1.14)
read-create
Unsigned32
Unsigned32(1.. 4096)
Ethernet service instance ID.
As per the MIB.
hh3cTwamplightClientDesMac(1.3.6.1.4.1.25506.2.184.2.1.3.1.15)
read-create
MacAddress
Destination MAC address of the probe packets.
As per the MIB.
hh3cTwamplightClientSrcMac(1.3.6.1.4.1.25506.2.184.2.1.3.1.16)
read-create
MacAddress
Source MAC address of the probe packets.
As per the MIB.
hh3cTwamplightClientTimeFormat(1.3.6.1.4.1.25506.2.184.2.1.3.1.17)
read-create
INTEGER
ntp (1),
ptp (2)
Timestamp format of the probe packets.
As per the MIB.
hh3cTwamplightClientDataFill(1.3.6.1.4.1.25506.2.184.2.1.3.1.18)
read-create
DisplayString
OCTET STRING(1..200)
Payload fill string.
As per the MIB.
hh3cTwamplightClientDataFillType(1.3.6.1.4.1.25506.2.184.2.1.3.1.19)
read-create
INTEGER
string (1),
hex (2)
Type of the payload fill string.
As per the MIB.
hh3cTwamplightClientSVlanID(1.3.6.1.4.1.25506.2.184.2.1.3.1.20)
read-create
Unsigned32
Unsigned32(1..4094)
Outer VLAN ID of the probe packets.
As per the MIB.
hh3cTwamplightClientCVlanID(1.3.6.1.4.1.25506.2.184.2.1.3.1.21)
read-create
Unsigned32
Unsigned32(1..4094)
Inner VLAN ID of the probe packets.
As per the MIB.
hh3cTwamplightClientVlanPriority(1.3.6.1.4.1.25506.2.184.2.1.3.1.22)
read-create
Unsigned32
Unsigned32(0..7)
802.1p priority of the probe packets.
As per the MIB.
hh3cTwamplightClientBindIfName(1.3.6.1.4.1.25506.2.184.2.1.3.1.23)
read-create
DisplayString
OCTET STRING(0..47)
Name of the interface to which the session binds.
As per the MIB.
hh3cTwamplightSenderAdminTable
About this table
Use this table to configure and obtain information about TWAMP light tests.
CreateSupported
DeleteSupported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cTwamplightSendAdminContinual(1.3.6.1.4.1.25506.2.184.2.1.4.1.1)
read-create
Integer32
TWAMP test type.
As per the MIB.
hh3cTwamplightSendAdminDuration(1.3.6.1.4.1.25506.2.184.2.1.4.1.2)
read-create
Integer32
Integer32(60..3600)
TWAMP test duration.
As per the MIB.
hh3cTwamplightSendAdminPktCount (1.3.6.1.4.1.25506.2.184.2.1.4.1.3)
read-create
Integer32
Integer32(100..30000)
Number of packets to send for the TWAMP test.
As per the MIB.
hh3cTwamplightSendAdminTxPeriod (1.3.6.1.4.1.25506.2.184.2.1.4.1.4)
read-create
INTEGER
interval10ms(1), interval100ms(2), interval1s(3), interval30s(4), interval10s(5)
Interval at which probe packets are sent for the TWAMP test.
Supports only interval10ms(1), interval100ms(2), interval1s(3), interval30s(4), and interval10s(5).
hh3cTwamplightSendAdminTimeOut (1.3.6.1.4.1.25506.2.184.2.1.4.1.5)
read-create
Integer32
Integer32(1..60)
Timeout time for TWAMP response packets.
hh3cTwamplightSendAdminRowStatus(1.3.6.1.4.1.25506.2.184.2.1.4.1.6)
read-create
RowStatus
Supports only createAndGo(4) and destroy(6).
hh3cTwamplightSenderStatusTable
About this table
Use this MIB to obtain the TWAMP Light sender status.
CreateNot supported
Edit/ModifyNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cTwamplightSenderStatus(1.3.6.1.4.1.25506.2.184.2.1.5.1.1)
read-only
INTEGER
inactive(1), active(2)
Operational state of a TWAMP test.
Supports only inactive(1) and active(2).
hh3cTwamplightSenderStatusType(1.3.6.1.4.1.25506.2.184.2.1.5.1.2)
read-only
INTEGER
init(0), continual(1), onDemand(2)
Operational type of a TWAMP test.
Supports only init(0), continual(1), and onDemand(2).
hh3cTwamplightLastStartTime(1.3.6.1.4.1.25506.2.184.2.1.5.1.4)
read-only
DateAndTime
Date and time when the most recent test started.
As per the MIB.
hh3cTwamplightLastStopTime(1.3.6.1.4.1.25506.2.184.2.1.5.1.5)
read-only
DateAndTime
Date and time when the most recent test stopped.
As per the MIB.
hh3cTwamplightTwoWayDelayTable
About this table
Use this table to obtain statistics result about TWAMP Light tests.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
The table indexes are hh3cTwamplightControllerID and hh3cTwamplightTWDelaySeq.
Object (OID)
Access
Value range
Implementation
hh3cTwamplightTWDelaySeq(1.3.6.1.4.1.25506.2.184.2.1.6.1.1)
read-only
Gauge32
Sequence number.
As per the MIB.
hh3cTwamplightTWDelayAvgDelay (1.3.6.1.4.1.25506.2.184.2.1.6.1.2)
read-only
Integer32
Average delay.
As per the MIB.
hh3cTwamplightTWDelayMaxDelay (1.3.6.1.4.1.25506.2.184.2.1.6.1.3)
read-only
Integer32
Maximum delay.
As per the MIB.
hh3cTwamplightTWDelayMinDelay (1.3.6.1.4.1.25506.2.184.2.1.6.1.4)
read-only
Integer32
Minimum delay.
As per the MIB.
hh3cTwamplightTWDelayAvgJitter(1.3.6.1.4.1.25506.2.184.2.1.6.1.5)
read-only
Integer32
Average jitter.
As per the MIB.
hh3cTwamplightTWDelayMaxJitter(1.3.6.1.4.1.25506.2.184.2.1.6.1.6)
read-only
Integer32
Maximum jitter.
As per the MIB.
hh3cTwamplightTWDelayMinJitter(1.3.6.1.4.1.25506.2.184.2.1.6.1.7)
read-only
Integer32
Minimum jitter.
As per the MIB.
hh3cTwamplightTWDelayAvgJitterSD (1.3.6.1.4.1.25506.2.184.2.1.6.1.8)
read-only
Integer32
Average jitter from source to destination.
As per the MIB.
hh3cTwamplightTWDelayMaxJitterSD (1.3.6.1.4.1.25506.2.184.2.1.6.1.9)
read-only
Integer32
Maximum jitter from source to destination.
As per the MIB.
hh3cTwamplightTWDelayMinJitterSD (1.3.6.1.4.1.25506.2.184.2.1.6.1.10)
read-only
Integer32
Minimum jitter from source to destination.
As per the MIB.
hh3cTwamplightTWDelayAvgJitterDS (1.3.6.1.4.1.25506.2.184.2.1.6.1.11)
read-only
Integer32
Average jitter from destination to source.
As per the MIB.
hh3cTwamplightTWDelayMaxJitterDS (1.3.6.1.4.1.25506.2.184.2.1.6.1.12)
read-only
Integer32
Maximum jitter from destination to source.
As per the MIB.
hh3cTwamplightTWDelayMinJitterDS (1.3.6.1.4.1.25506.2.184.2.1.6.1.13)
read-only
Integer32
Minimum jitter from destination to source.
As per the MIB.
hh3cTwamplightTwoWayLossTable
About this table
Use this table to obtain packet loss statistics for TWAMP Light tests.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
The table indexes are hh3cTwamplightControllerID and hh3cTwamplightTWLossSeq.
Object (OID)
Access
Value range
Implementation
hh3cTwamplightTWLossSeq(1.3.6.1.4.1.25506.2.184.2.1.7.1.1)
read-only
Gauge32
Sequence number.
As per the MIB.
hh3cTwamplightTWLossValue(1.3.6.1.4.1.25506.2.184.2.1.7.1.2)
read-only
Integer32
Number of lost packets in a statistical cycle of a TWAMP test.
As per the MIB.
hh3cTwamplightTWSentCount(1.3.6.1.4.1.25506.2.184.2.1.7.1.3)
read-only
Integer32
Number of sent packets in a statistical cycle of a TWAMP test.
As per the MIB.
hh3cTwamplightTWTotalLossValue(1.3.6.1.4.1.25506.2.184.2.1.7.1.4)
read-only
Integer32
Number of lost packets in the most recent 30 statistical cycle of a TWAMP test.
As per the MIB.
hh3cTwamplightTWTotalSentCount(1.3.6.1.4.1.25506.2.184.2.1.7.1.5)
read-only
Integer32
Number of sent packets in the most recent 30 statistical cycle of a TWAMP test.
As per the MIB.
hh3cTwamplightTWErrorCount(1.3.6.1.4.1.25506.2.184.2.1.7.1.6)
read-only
Unsigned32
Number of error packets received in a statistical cycle        of a TWAMP-light test.
As per the MIB.
hh3cTwamplightTWTotalErrorCount(1.3.6.1.4.1.25506.2.184.2.1.7.1.7)
read-only
Unsigned32
Number of error packets received in last 30 statistical        cycles of a TWAMP-light test.
As per the MIB.
hh3cTwamplightSenderLossSeqTable
About this table
Use this table to obtain the largest index value in TWAMP loss results.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cTwamplightLossSeqNumValue(1.3.6.1.4.1.25506.2.184.2.1.8.1.1)
read-only
Gauge32
Largest index value in TWAMP loss results.
As per the MIB.
hh3cTwamplightSendDelaySeqTable
About this table
Use this table to obtain the largest index value in TWAMP delay results.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cTwamplightSenderDelaySeqNum(1.3.6.1.4.1.25506.2.184.2.1.9.1.1)
read-only
Gauge32
Largest index value in TWAMP delay results.
As per the MIB.
hh3cTwamplightResetStatTable
About this table
Use this table to clear TWAMP Light test statistics.
CreateNot supported
DeleteNot supported
ReadNot supported
Columns
Object (OID)
Access
Value range
Implementation
hh3cTwamplightResetStatistics(1.3.6.1.4.1.25506.2.184.2.1.10.1.1)
read-create
INTEGER
single(1),
all(2)
Clears statistics for one or all TWAMP Light tests.
Supports only set operations.
Supports only single(1) and all(2).
hh3cTwamplightReactionTable
About this table
Use this table to configure and obtain information about a reaction entry.
CreateSupported
DeleteSupported
ReadSupported
Columns
The table indexes are hh3cTwamplightControllerID and hh3cTwamplightReactItemIndex.
Object (OID)
Access
Value range
Implementation
hh3cTwamplightReactItemIndex(1.3.6.1.4.1.25506.2.184.2.1.11.1.1)
Unsigned32
Integer32(1..10)
ID of a reaction entry
As per the MIB.
hh3cTwamplightReactCheckElement(1.3.6.1.4.1.25506.2.184.2.1.11.1.2)
read-create
INTEGER
twoWayDelay(1), twoWayJitter(2), twoWayLoss(3)
Monitored performance metric.
As per the MIB.
hh3cTwamplightReactUpperLimit(1.3.6.1.4.1.25506.2.184.2.1.11.1.3)
read-create
Unsigned32
Unsigned32(2..1000000)
Lower threshold limit.
As per the MIB.
hh3cTwamplightReactLowerLimit
(1.3.6.1.4.1.25506.2.184.2.1.11.1.4)
read-create
Integer32
Unsigned32(1..999999)
Upper threshold limit.
As per the MIB.
hh3cTwamplightReactActionType(1.3.6.1.4.1.25506.2.184.2.1.11.1.5)
read-create
INTEGER
none(0),
trapOnly(1)
Action for the threshold violation event.
As per the MIB.
hh3cTwamplightReactRowStatus(1.3.6.1.4.1.25506.2.184.2.1.11.1.6)
read-create
RowStatus
Controls the creation and deletion of the conceptual row.
Supports only active(1), createAndGo(4), and destroy(6).
hh3cTwamplightReactValue(1.3.6.1.4.1.25506.2.184.2.1.11.1.7)
Unsigned32
Unsigned32(1..1000000)
Threshold.
As per the MIB.
hh3cTwamplightResponderTable
About this table
Use this table to configure and obtain information about test sessions on the TWAMP Light responder.
CreateSupported
DeleteSupported
ReadSupported
Columns
The table index is hh3cTwamplightRespID.
Object (OID)
Access
Value range
Implementation
hh3cTwamplightRespID(1.3.6.1.4.1.25506.2.184.2.2.2.1.1)
not-accessible
Integer32
Integer32(1..512)
Test session ID.
hh3cTwamplightRespSrcAddrType(1.3.6.1.4.1.25506.2.184.2.2.2.1.2)
read-create
InetAddressType
As per the MIB.
hh3cTwamplightRespSrcAddr(1.3.6.1.4.1.25506.2.184.2.2.2.1.3)
read-create
InetAddress
Source IP address.
As per the MIB.
hh3cTwamplightRespTrgtAddrType(1.3.6.1.4.1.25506.2.184.2.2.2.1.4)
read-create
Integer32
As per the MIB.
hh3cTwamplightRespTrgtAddr(1.3.6.1.4.1.25506.2.184.2.2.2.1.5)
read-create
OCTET STRING
As per the MIB.
hh3cTwamplightRespSrcPort(1.3.6.1.4.1.25506.2.184.2.2.2.1.6)
read-create
Integer32
Integer32(1..65535)
Source port number.
As per the MIB.
hh3cTwamplightRespTrgtPort(1.3.6.1.4.1.25506.2.184.2.2.2.1.7)
read-create
Integer32
Integer32(1..65535)
As per the MIB.
hh3cTwamplightRespVPN(1.3.6.1.4.1.25506.2.184.2.2.2.1.8)
read-create
DisplayString
OCTET STRING(1..31)
As per the MIB.
hh3cTwamplightRespDescription(1.3.6.1.4.1.25506.2.184.2.2.2.1.9)
read-create
DisplayString
Description about the test session.
As per the MIB.
hh3cTwamplightRespRowStatus(1.3.6.1.4.1.25506.2.184.2.2.2.1.10)
read-create
RowStatus
active(1), createAndGo(4), destroy(6)
hh3cTwamplightRespSrcIfName(1.3.6.1.4.1.25506.2.184.2.2.2.1.11)
read-create
DisplayString
OCTET STRING(0..47)
Source interface of the reflected packets.
As per the MIB.
hh3cTwamplightRespServiceID(1.3.6.1.4.1.25506.2.184.2.2.2.1.12)
read-create
Unsigned32
Unsigned32(1..4096)
Ethernet service instance ID for the session.
As per the MIB.
hh3cTwamplightRespDesMac(1.3.6.1.4.1.25506.2.184.2.2.2.1.13)
read-create
MacAddress
Destination MAC address of the reflected packets.
As per the MIB.
hh3cTwamplightRespSrcMac(1.3.6.1.4.1.25506.2.184.2.2.2.1.14)
read-create
MacAddress
Source MAC address of the reflected packets.
As per the MIB.
hh3cTwamplightRespTimeFormat(1.3.6.1.4.1.25506.2.184.2.2.2.1.15)
read-create
INTEGER
auto(0)
ntp(1)
ptp(2)
Timestamp format of the reflected packets.
As per the MIB.
hh3cTwamplightRespSVlanID(1.3.6.1.4.1.25506.2.184.2.2.2.1.16)
read-create
Unsigned32
Unsigned32(1..4094)
Outer VLAN ID of the reflected packets.
As per the MIB.
hh3cTwamplightRespCVlanID(1.3.6.1.4.1.25506.2.184.2.2.2.1.17)
read-create
Unsigned32
Unsigned32(1..4094)
Inner VLAN ID of the reflected packets.
As per the MIB.
Notifications
hh3cTwampTwoWayLossExceed
Basic information
OID
Event
Severity
Recovery notification
Default status
1.3.6.1.4.1.25506.2.184.1.0.1
The two-way packet loss ratio exceeds the upper threshold.
Error
Warning
1.3.6.1.4.1.25506.2.184.1.0.2 (hh3cTwampTwoWayLossRecover)
OFF
Notification triggers
This notification is generated when the two-way packet loss ratio exceeds the upper threshold in the TWAMP test. Possible causes might include the following:
Cause 1: Network congestion due to abnormal traffic.
Cause 2: Unstable link state.
System impact
The packet loss rate is too high and might not meet the service requirements. Services are affected.
Status control
ON
CLI: Use the reaction item-number checked-element two-way-loss threshold-value upper-threshold lower-threshold action-type trap-only command.
OFF
CLI: Use the undo reaction item-number command.
Object
OID (object name)
Index
Value range
1.3.6.1.4.1.25506.2.184.2.1.3.1.1 (hh3cTwamplightControllerID)
Session ID.
Integer32
Integer32(1..512)
1.3.6.1.4.1.25506.2.184.2.1.11.1.1 (hh3cTwamplightReactItemIndex)
Threshold alarm group ID.
Unsigned32
Integer32(1..10)
1.3.6.1.4.1.25506.2.184.2.1.11.1.7 (hh3cTwamplightReactValue)
Threshold.
Unsigned32
1.3.6.1.4.1.25506.2.184.2.1.11.1.3 (hh3cTwamplightReactUpperLimit)
Upper threshold.
Unsigned32
1.3.6.1.4.1.25506.2.184.2.1.11.1.4 (hh3cTwamplightReactLowerLimit)
Lower threshold.
Integer32
Recommended action
To resolve this issue:
1.Identify whether abnormal traffic exists in the network during the alarm time.
2.Identify whether the link state is stable in the network during the alarm time, and troubleshoot link instability issues.
3.If the issue persists, collect alarm information and configuration data, and then contact H3C Support for help.
Basic information
OID
Event
Severity
Default status
The two-way packet loss ratio drops below the lower threshold.
Recovery
Warning
N/A (N/A)
OFF
This notification is generated when the two-way packet loss ratio drops below the lower threshold in the TWAMP test.
System impact
No negative impact on services.
Status control
ON
OFF
CLI: Use the reaction item-number checked-element two-way-loss threshold-value upper-threshold lower-threshold action-type trap-only none command.
Object
OID (object name)
Index
Value range
Session ID.
Integer32
Integer32(1..512)
Unsigned32
Integer32(1..10)
Threshold.
Unsigned32
Upper threshold.
Unsigned32
Lower threshold.
Integer32
Recommended action
No action is required.
hh3cTwampTwoWayDelayExceed
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.184.1.0.3
The two-way delay exceeds the upper threshold.
Error
Warning
1.3.6.1.4.1.25506.2.184.1.0.4 (hh3cTwampTwoWayDelayRecover)
OFF
This notification is generated when the two-way delay exceeds the upper threshold in the TWAMP test.
System impact
The delay is too high and might not meet the service requirements. Services are affected.
Status control
ON
CLI: Use the reaction item-number checked-element two-way-delay threshold-value upper-threshold lower-threshold action-type trap-only command.
OFF
Object
OID (object name)
Index
Value range
Session ID.
Integer32
Integer32(1..512)
Unsigned32
Integer32(1..10)
Threshold.
Unsigned32
Upper threshold.
Unsigned32
Lower threshold.
Integer32
Recommended action
Basic information
OID
Event
Severity
Default status
The two-way delay drops below the lower threshold.
Recovery
Warning
N/A (N/A)
OFF
This notification is generated when the two-way delay drops below the lower threshold in the TWAMP test.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Session ID.
Integer32
Integer32(1..512)
Unsigned32
Integer32(1..10)
Threshold.
Unsigned32
Upper threshold.
Unsigned32
Lower threshold.
Integer32
Recommended action
hh3cTwampTwoWayJitterExceed
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.184.1.0.5
The two-way jitter exceeds the upper threshold.
Error
Warning
1.3.6.1.4.1.25506.2.184.1.0.6 (hh3cTwampTwoWayJitterRecover)
OFF
This notification is generated when the two-way jitter exceeds the upper threshold in the TWAMP test.
System impact
The jitter is too high and might not meet the service requirements. Services are affected.
Status control
ON
CLI: Use the reaction item-number checked-element two-way-jitter threshold-value upper-threshold lower-threshold action-type trap-only command.
OFF
Object
OID (object name)
Index
Value range
Session ID.
Integer32
Integer32(1..512)
Unsigned32
Integer32(1..10)
Threshold.
Unsigned32
Upper threshold.
Unsigned32
Lower threshold.
Integer32
Recommended action
Basic information
OID
Event
Severity
Default status
The two-way jitter drops below the lower threshold.
Recovery
Warning
N/A (N/A)
OFF
This notification is generated when the two-way jitter drops below the lower threshold in the TWAMP test.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Session ID.
Integer32
Integer32(1..512)
Unsigned32
Integer32(1..10)
Threshold.
Unsigned32
Upper threshold.
Unsigned32
Lower threshold.
Integer32
Recommended action
hh3cTwampSenderSessionNumLimit
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.184.1.0.7
The number of TAWMP test sessions reaches the upper limit.
Informational
Major
N/A (N/A)
OFF
This notification is generated when the number of TAWMP test sessions reaches the upper limit.
System impact
The TAWMP test sessions that exceed the system capacity cannot operate correctly.
Status control
This notification cannot be disabled.
Object
OID (object name)
Index
Value range
N/A (N/A)
N/A
N/A
N/A
N/A
Recommended action
1.Execute the display nqa twamp-light client verbose command to check for inactive sessions.
  - If inactive sessions exist, delete the sessions.
  - If no inactive sessions exist, as a best practice, arrange services appropriately.
2.If the issue persists, collect alarm information and configuration data, and then contact H3C Support for help.
