07-Layer 3—IP Services Command Reference
HomeSupportReference GuidesCommand ReferencesH3C MSR1000[2600][3600] Routers Command Reference(V9)-R9119-6W10007-Layer 3—IP Services Command Reference
03-DHCP commands
03-DHCP commands 499.79 KB
DHCP commands· 1
Common DHCP commands· 1
dhcp client-detect 1
dhcp dscp· 1
dhcp enable· 2
dhcp log enable· 2
dhcp select 3
DHCP server commands· 4
address range· 4
allocate-new-ip enable· 5
bims-server 6
bootfile-name· 6
class ip-pool 7
class option-group· 8
class range· 9
default ip-pool 10
dhcp apply-policy· 11
dhcp class· 11
dhcp option-group· 12
dhcp policy· 13
dhcp server allocated-ip threshold· 13
dhcp server always-broadcast 14
dhcp server apply ip-pool 15
dhcp server bootp ignore· 15
dhcp server bootp reply-rfc-1048· 16
dhcp server check mac-address· 17
dhcp server database filename· 17
dhcp server database update interval 19
dhcp server database update now· 19
dhcp server database update stop· 20
dhcp server forbidden-ip· 21
dhcp server ip-pool 22
dhcp server multi-ip per-mac enable· 22
dhcp server ping packets· 23
dhcp server ping timeout 24
dhcp server relay information enable· 24
dhcp server reply-exclude-option60· 25
dhcp server request-ip-address check· 26
display dhcp server conflict 26
display dhcp server database· 27
display dhcp server expired· 28
display dhcp server free-ip· 30
display dhcp server ip-in-use· 31
display dhcp server pool 33
display dhcp server statistics· 36
dns-list 38
domain-name· 39
expired· 39
forbidden-ip· 40
forbidden-ip-range· 41
gateway-list 42
if-match· 43
ip-in-use threshold· 45
nbns-list 46
netbios-type· 47
network· 48
next-server 49
option· 50
reserve expired-ip enable· 51
reserve expired-ip mode· 52
reset dhcp server conflict 53
reset dhcp server expired· 54
reset dhcp server ip-in-use· 54
reset dhcp server statistics· 55
snmp-agent trap enable dhcp server 55
static-bind· 56
subnet alloc-mode· 58
subnet export-route disable· 58
subnet idle-time· 59
subnet mask-length· 60
tftp-server domain-name· 60
tftp-server ip-address· 61
valid class· 62
verify class· 62
voice-config· 63
vpn-instance· 64
DHCP relay agent commands· 65
dhcp relay always-unicast 65
dhcp relay check mac-address· 65
dhcp relay check mac-address aging-time· 66
dhcp relay client-information record· 67
dhcp relay client-information refresh· 67
dhcp relay client-information refresh enable· 68
dhcp relay dhcp-server timeout 69
dhcp relay forward reply by-option82· 70
dhcp relay gateway· 70
dhcp relay information circuit-id· 71
dhcp relay information enable· 73
dhcp relay information remote-id· 74
dhcp relay information strategy· 75
dhcp relay mac-forward enable· 76
dhcp relay master-server switch-delay· 77
dhcp relay release ip· 77
dhcp relay request-from-tunnel discard· 78
dhcp relay server-address· 78
dhcp relay server-address algorithm·· 79
dhcp relay source-address· 80
dhcp-server timeout 82
dhcp smart-relay enable· 82
display dhcp relay check mac-address· 83
display dhcp relay client-information· 84
display dhcp relay information· 86
display dhcp relay server-address· 87
display dhcp relay statistics· 88
gateway-list 89
master-server switch-delay· 90
remote-server 91
remote-server algorithm·· 91
reset dhcp relay client-information· 92
reset dhcp relay statistics· 93
DHCP client commands· 93
dhcp client dad enable· 93
dhcp client dscp· 94
dhcp client identifier 94
display dhcp client 95
ip address dhcp-alloc· 98
BOOTP client commands· 98
display bootp client 98
ip address bootp-alloc· 99
DHCP commands
dhcp client-detect
Use dhcp client-detect to enable client offline detection on the DHCP server or DHCP relay agent.
Use undo dhcp client-detect to disable client offline detection on the DHCP server or DHCP relay agent.
dhcp client-detect
Client offline detection is disabled on the DHCP server or DHCP relay agent.
Interface view
The client offline detection feature on the DHCP server reclaims an assigned IP address and deletes the binding entry when the ARP entry ages out for the IP address.
This feature on the DHCP relay agent deletes the related relay entry and sends a RELEASE message to the DHCP server when an ARP entry ages out.
# Enable client offline detection.
[Sysname] interface gigabitethernet 0/0/1
[Sysname-GigabitEthernet0/0/1] dhcp client-detect
dhcp dscp
Use dhcp dscp to set the DSCP value for DHCP packets sent by the DHCP server or the DHCP relay agent.
Use undo dhcp dscp to restore the default.
dhcp dscp dscp-value
undo dhcp dscp
The DSCP value is 56 in DHCP packets sent by the DHCP server or the DHCP relay agent.
dscp-value: Specifies the DSCP value for DHCP packets, in the range of 0 to 63.
The DSCP value of a packet specifies the priority level of the packet and affects the transmission priority of the packet. A bigger DSCP value represents a higher priority.
# Set the DSCP value to 30 for DHCP packets sent by the DHCP server or the DHCP relay agent.
[Sysname] dhcp dscp 30
dhcp enable
Use dhcp enable to enable DHCP.
Use undo dhcp enable to disable DHCP.
dhcp enable
undo dhcp enable
DHCP is disabled.
DHCP related configuration takes effect only after you enable DHCP.
Enable DHCP before you configure the DHCP server or relay agent.
# Enable DHCP.
[Sysname] dhcp enable
dhcp log enable
Use dhcp log enable to enable DHCP server logging.
Use undo dhcp log enable to disable DHCP server logging.
dhcp log enable
DHCP server logging is disabled.
This command enables the DHCP server to generate DHCP logs and send them to the information center. For information about the log destination and output rule configuration in the information center, see System Management Configuration Guide.
As a best practice, disable this feature if the log generation affects the device performance or reduces the address allocation efficiency. For example, this situation might occur when a large number of clients frequently come online or go offline.
# Enable DHCP server logging.
[Sysname] dhcp log enable
dhcp select
Use dhcp select to enable the DHCP server or DHCP relay agent on an interface.
Use undo dhcp select to disable the DHCP server or DHCP relay agent on an interface. The interface will discard incoming DHCP packets.
dhcp select { relay [ proxy ] | server }
undo dhcp select { relay | server }
The interface operates in the DHCP server mode and responds to DHCP requests with configuration parameters.
Interface view
relay: Enables the DHCP relay agent on the interface.
proxy: Enables the DHCP server proxy on the relay agent.
server: Enables the DHCP server on the interface.
Before enabling a DHCP server to operate as a DHCP relay agent, use the reset dhcp server ip-in-use command to clear address bindings and authorized ARP entries. These authorized ARP entries might conflict with ARP entries that are created after the DHCP relay agent is enabled.
When DHCP server proxy is enabled on the DHCP relay agent, the proxy forwards packets between the DHCP clients and DHCP server.
·     When receiving DHCP requests from DHCP clients, the proxy forwards them to the DHCP server.
·     When receiving DHCP responses from the DHCP server, the proxy modifies the DHCP server's IP address in these responses as its own IP address.
# Enable the DHCP relay agent on GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp select relay
·     dhcp relay always-unicast
·     dhcp server request-ip-address check
address range
Use address range to configure an IP address range in a DHCP address pool for dynamic allocation.
Use undo address range to restore the default.
undo address range
No IP address range exists.
DHCP address pool view
start-ip-address: Specifies the start IP address.
end-ip-address: Specifies the end IP address.
If no IP address range is specified, all IP addresses in the subnet specified by the network command in address pool view are assignable. If an IP address range is specified, only the IP addresses in the IP address range are assignable.
After you use the address range command, you cannot use the network secondary command to specify a secondary subnet in the address pool.
The address range specified by the address range command must be within the subnet specified by the network command. The addresses outside of the subnet cannot be assigned.
# Specify an address range of 192.168.8.1 through 192.168.8.150 in address pool 1.
[Sysname] dhcp server ip-pool 1
[Sysname-dhcp-pool-1] network 192.168.8.1 mask 255.255.255.0
[Sysname-dhcp-pool-1] address range 192.168.8.1 192.168.8.150
class
dhcp class
network
Use allocate-new-ip enable to enable random IP address allocation.
Use undo allocate-new-ip enable to disable random IP address allocation.
Random IP address allocation is disabled.
By default, the DHCP server tries to allocate the same IP address as the previous allocation to the same user.
With this feature enabled, the DHCP server tries to allocate a new IP address to a user every time the user acquires an IP address. This feature is applicable to the scenarios where each user is identified by IP address. In such a network scenario, it is required that a user must obtain different IP addresses for each IP address acquisition.
# Enable random IP address allocation.
[Sysname-dhcp-pool-1] allocate-new-ip enable
This command will enable the random address allocation mode. Enable it? [Y/N]:
bims-server
Use bims-server to specify the IP address, port number, and shared key of the BIMS server in a DHCP address pool.
Use undo bims-server to restore the default.
undo bims-server
No BIMS server information is specified.
ip ip-address: Specifies the IP address of the BIMS server.
port port-number: Specifies the port number of the BIMS server, in the range of 1 to 65534.
simple: Specifies a key in plaintext form. For security purposes, the key specified in plaintext form will be stored in encrypted form.
string: Specifies the key string. Its plaintext form is a case-sensitive string of 1 to 16 characters. Its encrypted form is a case-sensitive string of 1 to 53 characters. The DHCP client uses the shared key to encrypt packets sent to the BIMS server.
# Specify BIMS server IP address 1.1.1.1, port number 80, and shared key aabbcc in address pool 0.
[Sysname] dhcp server ip-pool 0
[Sysname-dhcp-pool-0] bims-server ip 1.1.1.1 port 80 sharekey simple aabbcc
bootfile-name
Use bootfile-name to specify a configuration file name or URL.
Use undo bootfile-name to restore the default.
bootfile-name { bootfile-name | url }
undo bootfile-name
No configuration file name or URL is specified.
bootfile-name: Specifies the configuration file name, a case-sensitive string of 1 to 63 characters.
url: Specifies the HTTP URL of the configuration file. It is a case-sensitive string of 1 to 63 characters.
To specify a configuration file on a TFTP server, use the bootfile-name argument.
To specify a configuration file on an HTTP server, use the url argument.
# Specify configuration file name boot.cfg in DHCP address pool 0.
[Sysname-dhcp-pool-0] bootfile-name boot.cfg
# Specify configuration file URL http://10.1.1.1/boot.cfg in DHCP address pool 0.
[Sysname-dhcp-pool-0] bootfile-name http://10.1.1.1/boot.cfg
next-server
class ip-pool
Use class ip-pool to specify a DHCP address pool for a DHCP user class.
Use undo class ip-pool to remove the DHCP address pool specified for a DHCP user class.
undo class class-name ip-pool
No DHCP address pool is specified for a DHCP user class.
DHCP policy view
class-name: Specifies a DHCP user class by its name, a case-insensitive string of 1 to 63 characters.
pool-name: Specifies a DHCP address pool by its name, a case-insensitive string of 1 to 63 characters.
You can specify only one DHCP address pool for a DHCP user class in a DHCP policy. If you execute this command multiple times for a user class, the most recent configuration takes effect.
# Specify DHCP address pool pool1 for DHCP user class test in DHCP policy 1.
[Sysname] dhcp policy 1
[Sysname-dhcp-policy-1] class test ip-pool pool1
default ip-pool
dhcp policy
dhcp server ip-pool
class option-group
Use class option-group to specify a DHCP option group for a DHCP user class.
Use undo class option-group to remove the configuration.
undo class class-name option-group
No DHCP option group is specified for a DHCP user class.
option-group-number: Specifies a DHCP option group by its number in the range of 1 to 32768.
When receiving a DHCP-DISCOVER message, the server compares the client against the user classes in the order that they are specified by this command. If a match is found, the server assigns the client the DHCP options in the option group. If multiple matches are found, the server selects option groups by using the following methods:
·     If the option groups have options in common, the server selects the option group specified for the first matching user class.
·     If the option groups have different options, the server selects all the matching option groups.
You can specify only one option group for a DHCP user class in a DHCP address pool. If you execute this command multiple times for a user class, the most recent configuration takes effect.
# Specify DHCP option group 1 for user class user in DHCP address pool 0.
[Sysname-dhcp-pool-0] class user option-group 1
dhcp option-group
class range
Use class range to specify an IP address range for a DHCP user class.
Use undo class range to remove the IP address range for the DHCP user class.
undo class class-name range
No IP address range is specified for a DHCP user class.
class-name: Specifies a DHCP user class name, a case-insensitive string of 1 to 63 characters. If the specified user class does not exist, the DHCP server will not assign the addresses in the address range specified for the user class to any clients.
The class range command allows you to divide an address range into multiple address ranges for different DHCP user classes. The address range for a user class must be within the primary subnet specified by the network command. If the DHCP client does not match any DHCP user class, the DHCP server selects an address in the IP address range specified by the address range command. If the address range has no assignable IP addresses or no address range is configured, the address allocation fails.
After you specify an address range for a user class, you cannot use the network secondary command to specify a secondary subnet in the address pool.
You can specify only one address range for a DHCP user class in an address pool. If you execute this command multiple times for a DHCP user class, the most recent configuration takes effect.
# Specify an IP address range of 192.168.8.1 through 192.168.8.150 for DHCP user class user in DHCP address pool 1.
[Sysname-dhcp-pool-1] class user range 192.168.8.1 192.168.8.150
address range
dhcp class
default ip-pool
Use default ip-pool to specify the default DHCP address pool.
Use undo default ip-pool to restore the default.
default ip-pool pool-name
No default DHCP address pool is specified.
DHCP policy view
In a DHCP policy, the DHCP server uses the default DHCP address pool to assign IP addresses and other parameters to clients that do not match any user classes. If no default address pool is specified or the default address pool does not have assignable IP addresses, the address assignment fails.
You can specify only one default address pool in a DHCP policy. If you execute this command multiple times, the most recent configuration takes effect.
# Specify DHCP address pool pool1 as the default DHCP address pool in DHCP policy 1.
[Sysname-dhcp-policy-1] default ip-pool pool1
class ip-pool
dhcp policy
dhcp apply-policy
Use dhcp apply-policy to apply a DHCP policy to an interface.
Use undo dhcp apply-policy to restore the default.
dhcp apply-policy policy-name
No DHCP policy is applied to an interface.
Interface view
policy-name: Specifies a DHCP policy by its name, a case-insensitive string of 1 to 63 characters.
You can apply only one DHCP policy to an interface. If you execute this command multiple times, the most recent configuration takes effect.
# Apply DHCP policy test to GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp apply-policy test
dhcp policy
dhcp class
Use dhcp class to create a DHCP user class and enter its view, or enter the view of an existing DHCP user class.
Use undo dhcp class to delete the specified DHCP user class.
dhcp class class-name
undo dhcp class class-name
No DHCP user classes exist.
class-name: Specifies the name of a DHCP user class, a case-insensitive string of 1 to 63 characters.
In the DHCP user class view, you can use the if-match command to configure match rules to group clients to the user class.
# Create DHCP user class test and enter DHCP user class view.
[Sysname] dhcp class test
[Sysname-dhcp-class-test]
address range
class ip-pool
class option-group
class range
dhcp policy
if-match
dhcp option-group
Use dhcp option-group to create a DHCP option group and enter its view, or enter the view of an existing DHCP option group.
Use undo dhcp option-group to delete a DHCP option group.
undo dhcp option-group option-group-number
No DHCP option groups exist.
option-group-number: Assigns a number to the DHCP option group, in the range of 1 to 32768.
# Create DHCP option group 1 and enter DHCP option group view.
[Sysname] dhcp option-group 1
[Sysname-dhcp-option-group-1]
class option-group
option
dhcp policy
Use dhcp policy to create a DHCP policy and enter its view, or enter the view of an existing DHCP policy.
Use undo dhcp policy to delete a DHCP policy.
dhcp policy policy-name
undo dhcp policy policy-name
No DHCP policies exist.
policy-name: Assigns a name to the DHCP policy. The policy name is a case-insensitive string of 1 to 63 characters.
In DHCP policy view, you can specify address pools for different user classes. Clients matching a user class will obtain IP addresses and other parameters from the specified address pool.
For a DHCP policy to take effect, you must apply it to an interface.
# Create DHCP policy test and enter its view.
[Sysname] dhcp policy test
[Sysname-dhcp-policy-test]
class ip-pool
default ip-pool
dhcp apply-policy
dhcp class
Use dhcp server allocated-ip threshold to set the IP address allocation success rate threshold. The success rate is the rate of successfully allocated IP addresses to received DHCP requests within 5 minutes.
Use undo dhcp server allocated-ip threshold to restore the default.
dhcp server allocated-ip threshold threshold-value
No SNMP notification is sent for an IP address allocation success rate threshold violation.
threshold-value: Specifies the success rate threshold in percentage in the range of 1 to 100.
If the IP address allocation success rate is lower than the threshold, the DHCP module sends an SNMP notification to report the event.
# Set the IP address allocation success rate threshold to 85%.
[Sysname] dhcp server allocated-ip threshold 85
Use dhcp server always-broadcast to enable the DHCP server to always broadcast responses.
Use undo dhcp server always-broadcast to restore the default.
The DHCP server reads the broadcast flag in a DHCP request to decide whether to broadcast or unicast the response.
This command enables the DHCP server to ignore the broadcast flag in DHCP requests and always broadcast all responses.
The DHCP server always unicasts a response in the following situations, regardless of whether this command is executed:
·     The DHCP request is from a DHCP client that has an IP address (the ciaddr field is not 0).
·     The DHCP request is forwarded by a DHCP relay agent from a DHCP client (the giaddr field is not 0).
# Enable the DHCP server to always broadcast all responses.
[Sysname] dhcp server always-broadcast
Use dhcp server apply ip-pool to apply an address pool to an interface.
Use undo dhcp server apply ip-pool to restore the default.
No address pool is applied to an interface
Interface view
pool-name: Specifies the name of a DHCP address pool, a case-insensitive string of 1 to 63 characters.
Upon receiving a DHCP request from the interface, the DHCP server searches for a static binding for the client from all address pools. If no static binding is found, the server assigns configuration parameters from the address pool applied on the interface to the client. If the address pool has no assignable IP address or does not exist, the DHCP client cannot obtain an IP address.
# Apply DHCP address pool 0 to GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp server apply ip-pool 0
dhcp server ip-pool
Use dhcp server bootp ignore to configure the DHCP server to ignore BOOTP requests.
Use undo dhcp server bootp ignore to restore the default.
The DHCP server does not ignore BOOTP requests.
The lease duration of IP addresses obtained by BOOTP clients is unlimited. For scenarios that do not allow unlimited leases, you can configure the DHCP server to ignore BOOTP requests.
# Configure the DHCP server to ignore BOOTP requests.
[Sysname] dhcp server bootp ignore
Use dhcp server bootp reply-rfc-1048 to enable the sending of BOOTP responses in RFC 1048 format.
Use undo dhcp server bootp reply-rfc-1048 to disable this feature.
This feature is disabled. The DHCP server does not process the Vend field of RFC 1048-incompliant requests but copies the Vend field into responses.
Not all BOOTP clients can send requests compliant with RFC 1048. This command enables the DHCP server to fill the Vend field in RFC 1048-compliant format in DHCP responses to RFC 1048-incompliant requests sent by BOOTP clients.
# Enable the sending of BOOTP responses in RFC 1048 format on the DHCP server.
[Sysname] dhcp server bootp reply-rfc-1048
Use dhcp server check mac-address to enable MAC address check on the DHCP server.
Use undo dhcp server check mac-address to disable MAC address check on the DHCP server.
MAC address check is disabled on the DHCP server.
Interface view
This feature enables the DHCP server to compare the chaddr field of a received DHCP request with the source MAC address in the frame header. If they are the same, the DHCP server verifies the packet legal and continues processing the packet. If they are not the same, the DHCP server discards the request.
# Enable MAC address check on the DHCP server.
[Sysname-GigabitEthernet0/0/1] dhcp server check mac-address
Use dhcp server database filename to configure the DHCP server to back up the DHCP bindings to a file.
Use undo dhcp server database filename to restore the default.
The DHCP server does not back up the DHCP bindings.
filename: Specifies the name of a local backup file. For information about the filename argument, see Fundamentals Configuration Guide.
url url: Specifies the URL of a remote backup file, a case-sensitive string of 1 to 255 characters. Do not include a username or password in the URL.
username username: Specifies the username for accessing the URL of the remote backup file, a case-sensitive string of 1 to 32 characters. Do not specify this option if a username is not required for accessing the URL of the remote backup file.
string: Specifies the password. Its plaintext form is a case-sensitive string of 1 to 32 characters. Its encrypted form is a case-sensitive string of 1 to 73 characters. Do not specify this argument if a password is not required for accessing the URL of the remote backup file.
The command automatically creates the file if you specify a nonexistent file.
With this command executed, the DHCP server backs up its bindings immediately and runs auto backup. The server, by default, waits 300 seconds after a binding change to update the backup file. You can use the dhcp server database update interval command to change the waiting time. If no DHCP binding changes, the backup file is not updated.
As a best practice, back up the bindings to a remote file. If you use the local storage medium, the frequent erasing and writing might damage the medium and then cause the DHCP server to malfunction.
When the backup file is on a remote device, follow these restrictions and guidelines:
·     If the file is on an FTP server, enter URL in the following format: ftp://server address:port/file path, where the port number is optional.
·     The username and password must be the same as those configured on the FTP server. If the server authenticates only the username, the password can be omitted.
·     If the file is on a TFTP server, enter URL in the following format: tftp://server address:port/file path, where the port number is optional.
·     If the IP address of the server is an IPv6 address, enclose the address in a pair of brackets, for example, ftp://[1::1]/database.dhcp.
·     You can also specify the DNS domain name for the server address field, for example, ftp://company/database.dhcp.
# Configure the DHCP server to back up its bindings to file database.dhcp.
[Sysname] dhcp server database filename database.dhcp
# Configure the DHCP server to back up its bindings to file database.dhcp in the working directory of the FTP server at 10.1.1.1.
[Sysname] dhcp server database filename url ftp://10.1.1.1/database.dhcp username 1 password simple 1
Use dhcp server database update interval to set the waiting time for the DHCP server to update the backup file after a DHCP binding change.
Use undo dhcp server database update interval to restore the default.
The DHCP server waits 300 seconds to update the backup file after a DHCP binding change. If no DHCP binding changes, the backup file is not updated.
interval: Specifies the waiting time in the range of 60 to 864000 seconds.
When a DHCP binding is created, updated, or removed, the waiting period starts. The DHCP server updates the backup file when the waiting period is reached. All bindings changed during the period will be saved to the backup file.
The waiting time takes effect only after you configure the DHCP binding auto backup by using the dhcp server database filename command.
# Set the waiting time to 10 minutes for the DHCP server to update the backup file.
[Sysname] dhcp server database update interval 600
Use dhcp server database update now to manually save the DHCP bindings to the backup file.
Each time this command is executed, the DHCP bindings are saved to the backup file.
For this command to take effect, you must configure the DHCP auto backup by using the dhcp server database filename command.
# Manually save the DHCP bindings to the backup file.
[Sysname] dhcp server database update now
Use dhcp server database update stop to terminate the download of DHCP bindings from the backup file.
The DHCP server does not provide services during the binding download process. If the connection disconnects during the process, the waiting timeout timer is 60 minutes. When the timer expires, the DHCP server stops waiting and starts providing address allocation services.
To enable the DHCP server to provide services without waiting for the connection to be repaired, use this command to terminate the download immediately. The IP addresses associated with the undownloaded bindings will be assigned to clients. Address conflicts might occur.
# Terminate the download of the backup DHCP bindings.
[Sysname] dhcp server database update stop
Use dhcp server forbidden-ip to exclude IP addresses from dynamic allocation globally.
Use undo dhcp server forbidden-ip to remove the configuration.
undo dhcp server forbidden-ip start-ip-address [ end-ip-address ] [ vpn-instance vpn-instance-name ]
No IP addresses are excluded from dynamic allocation globally.
end-ip-address: Specifies the end IP address, which cannot be lower than the start-ip-address. If you do not specify this argument, only the start-ip-address is excluded from dynamic allocation.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If the excluded IP addresses belong to the public network, do not specify this option.
The IP addresses of some devices such as the gateway and FTP server cannot be assigned to clients. Use this command to exclude such addresses from dynamic allocation.
If the excluded IP address is in a static DHCP binding, the address can still be assigned to the client.
The address or address range specified in the undo dhcp server forbidden-ip command must be the same as that specified in the dhcp server forbidden-ip command. To remove an IP address from the specified address range, you must remove the entire address range.
You can execute this command multiple times to exclude multiple IP address ranges from dynamic allocation.
# Exclude the IP addresses of 10.110.1.1 through 10.110.1.63 from dynamic allocation globally.
[Sysname] dhcp server forbidden-ip 10.110.1.1 10.110.1.63
forbidden-ip
static-bind
dhcp server ip-pool
Use dhcp server ip-pool to create a DHCP address pool and enter its view, or enter the view of an existing DHCP address pool.
Use undo dhcp server ip-pool to delete the specified DHCP address pool.
dhcp server ip-pool pool-name [ subnet-alloc ]
undo dhcp server ip-pool pool-name
No DHCP address pools exist.
pool-name: Specifies a DHCP address pool name, a case-insensitive string of 1 to 63 characters. The pool name uniquely identifies an address pool.
subnet-alloc: Supports dynamic subnet allocation. If you do not specify this keyword, the command creates a DHCP address pool that does not support dynamic subnet allocation.
A DHCP address pool is used to store the configuration parameters to be assigned to DHCP clients.
# Create a DHCP address pool named pool1.
[Sysname] dhcp server ip-pool pool1
[Sysname-dhcp-pool-pool1]
class ip-pool
Use dhcp server multi-ip per-mac enable to enable allocation of different IP addresses to DHCP clients with the same MAC address.
Use undo dhcp server multi-ip per-mac enable to disable allocation of different IP addresses to DHCP clients with the same MAC address.
If the DHCP server has assigned IP addresses to DHCP clients, you cannot enable or disable this feature. If you do so, the system displays an error message.
# Enable allocation of different IP addresses to DHCP clients with the same MAC address.
[Sysname] dhcp server multi-ip per-mac enable
Use dhcp server ping packets to set the maximum number of ping packets.
Use undo dhcp server ping packets to restore the default.
The maximum number of ping packets is 1.
number: Sets the maximum number of ping packets, in the range of 0 to 10. To disable the address conflict detection, set the value to 0.
To avoid IP address conflicts, the DHCP server pings an IP address before assigning it to a DHCP client.
If a ping attempt succeeds, the server determines that the IP address is in use and picks a new IP address. If all the ping attempts fail, the server assigns the IP address to the requesting DHCP client.
# Set the maximum number of ping packets to 10.
[Sysname] dhcp server ping packets 10
Use dhcp server ping timeout to set the ping response timeout time on the DHCP server.
Use undo dhcp server ping timeout to restore the default.
The ping response timeout time is 500 milliseconds.
milliseconds: Specifies the timeout time in the range of 0 to 10000 milliseconds. To disable the ping operation for address conflict detection, set the value to 0 milliseconds.
# Set the response timeout time to 1000 milliseconds.
[Sysname] dhcp server ping timeout 1000
Use dhcp server relay information enable to enable the DHCP server to handle Option 82.
Use undo dhcp server relay information enable to configure the DHCP server to ignore Option 82.
The DHCP server handles Option 82.
Upon receiving a DHCP request that contains Option 82, the server copies the original Option 82 into the response. If the server is configured to ignore Option 82, the response will not contain Option 82.
# Configure the DHCP server to ignore Option 82.
[Sysname] undo dhcp server relay information enable
Use dhcp server reply-exclude-option60 to disable the DHCP server from encapsulating Option 60 in DHCP replies.
Use undo dhcp server reply-exclude-option60 to restore the default.
The DHCP server can encapsulate Option 60 in DHCP replies.
If you do not disable the capability, the DHCP server encapsulates Option 60 in a DHCP reply in the following situations:
·     The received DHCP packet contains Option 60.
·     Option 60 is configured for the address pool.
If you disable the capability, the DHCP server does not encapsulate Option 60 in DHCP replies.
# Disable the DHCP server from encapsulating Option 60 in DHCP replies.
[Sysname] dhcp server reply-exclude-option60
Use dhcp server request-ip-address check to enable the DHCP server to return a DHCP-NAK message if the client notions of their IP addresses are incorrect.
Use undo dhcp server request-ip-address check to restore the default.
The DHCP server does not return a DHCP-NAK message if the client notions of their IP addresses are incorrect.
A DHCP client can send a DHCP-REQUEST message directly or upon receiving a DHCP-OFFER message. Upon receiving the request, the DHCP server will check if the client notion of its IP address is correct. If the requested IP address is different from the allocated one or has no matching lease record, the DHCP server remains silent by default. After the allocated IP address lease for the client expires, the DHCP server will make response to request from the client.
This feature enables the DHCP server to return DHCP-NAK messages if the client notions of their IP addresses are incorrect. After receiving the DHCP-NAK message, the DHCP client will request an IP address again.
# Enable the DHCP server to return a DHCP-NAK message if the client notions of their IP addresses are incorrect.
[Sysname] dhcp server request-ip-address check
dhcp select server
Use display dhcp server conflict to display information about IP address conflicts.
display dhcp server conflict [ dp-address ip-address | ip ip-address | vxlan vxlan-id ] [ vpn-instance vpn-instance-name ]
dp-address ip-address: Specifies a DP by its IP address.
ip ip-address: Displays conflict information about the specified IP address.
vxlan vxlan-id: Specifies a VXLAN by its ID.
The DHCP server generates IP address conflict information in the following situations:
·     Before assigning an IP address to a DHCP client, the DHCP server pings the IP address and discovers that another host is using the address.
·     The DHCP client sends a DECLINE packet to the DHCP server to inform the server of an IP address conflict.
·     The DHCP server discovers that the only assignable address in the address pool is its own IP address.
If you do not specify any parameters, this command displays information about all IP address conflicts.
# Display information about all IP address conflicts.
<Sysname> display dhcp server conflict
IP address          Detect time
4.4.4.1             Apr 25 16:57:20 2019
4.4.4.2             Apr 25 17:00:10 2019
IP address
Conflicted IP address.
Detect time
Time when the conflict was discovered.
Use display dhcp server database to display information about DHCP binding auto backup.
# Display information about DHCP binding auto backup.
<Sysname> display dhcp server database
 Username                :
 Password                :
 Latest write time       :   Feb  8 16:09:53 2014
File name
Name of the DHCP binding backup file.
Username
Username for accessing the URL of the remote backup file.
Password
Password for accessing the URL of the remote backup file. This field displays ****** if a password is configured.
Update interval
Waiting time in seconds after a DHCP binding change for the DHCP server to update the backup file.
Latest write time
Time of the latest update.
Status
Status of the update:
·     Writing—The backup file is being updated.
·     Last write succeeded—The backup file was successfully updated.
·     Last write failed—The backup file failed to be updated.
Use display dhcp server expired to display the lease expiration information.
display dhcp server expired [  dp-address ip-address | ip ip-address | mac mac-address | vxlan vxlan-id | pool pool-name ] [ verbose ]
ip ip-address: Displays lease expiration information about the specified IP address.
mac mac-address: Specifies a MAC address.
pool pool-name: Displays lease expiration information about the specified address pool. The pool name is a case-insensitive string of 1 to 63 characters.
verbose: Displays detailed lease expiration information. If you do not specify this keyword, the command displays brief lease expiration information about all IP addresses.
DHCP assigns these expired IP addresses to DHCP clients when all available addresses have been assigned.
If you do not specify any parameters, this command displays lease expiration information about all IP addresses.
# Display all lease expiration information.
<Sysname> display dhcp server expired
IP address       Client-identifier/Hardware address    Lease expiration
4.4.4.6          3030-3066-2e65-3230-302e-3130-3234    Apr 25 17:10:47 2019
                 -2d45-7468-6572-6e65-7430-2f31
IP address
Expired IP address.
Client ID or MAC address.
Lease expiration
Time when the lease expired.
# Display detailed lease expiration information about all IP addresses.
<Sysname> display dhcp server expired verbose
IP address: 192.168.56.3
  Pool name: 1
  Client-identifier: N/A
  Hardware address type: Ethernet
  Hardware address: 0000-0000-0002
  Lease expiration: Mar 16 16:00:22 2017
  Remaining reservation time: 136 years 2 months 6 hours 28 minutes 11 seconds
  IP address reservation mode: Based on client MAC
IP address: 5.5.5.5
  Pool name: 2
  Client-identifier: 0061-6161-612e-6161-6161-2e61-6161-612d-4745-302f-302f-33
  Hardware address: 0000-0000-0003
  Lease expiration: Mar 16 16:00:33 2017
  Remaining reservation time: 136 years 2 months 6 hours 28 minutes 22 seconds
  IP address reservation mode: Based on client ID
IP address: 3.3.3.5
  Pool name: abc
  Client-identifier: 0100-0000-0000-05
  Hardware address: 0000-0000-0005
  Lease expiration: Mar 16 16:10:33 2017
  Remaining reservation time: 2 months 6 hours 27 minutes 22 seconds
IP address
Expired IP address.
Pool name
Address pool to which the expired IP address belongs.
Client-identifier
Client ID. If the request does not contain Option 61, this field displays N/A.
Hardware address type of the client: Ethernet, Token ring, or Unknown.
Lease expiration
Remaining time for reserving the expired IP address. If the reservation time expires, this field displays 0, and the expired IP address is deleted.
Reservation mode of the expired IP address:
·     Based on client ID—Reserve an expired IP address based on the client ID.
·     Based on client MAC—Reserve an expired IP address based on the client MAC address.
·     reserve expired-ip enable
Use display dhcp server free-ip to display information about assignable IP addresses.
pool pool-name: Displays assignable IP addresses in the specified address pool. The pool name is a case-insensitive string of 1 to 63 characters. If you do not specify an address pool, this command displays all assignable IP addresses for all address pools.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays assignable IP addresses in address pools for the public network.
# Display assignable IP addresses in all address pools.
<Sysname> display dhcp server free-ip
Pool name: 1
  Network: 10.0.0.0 mask 255.0.0.0
    IP ranges from 10.0.0.10 to 10.0.0.100
    IP ranges from 10.0.0.105 to 10.0.0.255
  Secondary networks:
    10.1.0.0 mask 255.255.0.0
      IP ranges from 10.1.0.0 to 10.1.0.255
    10.2.0.0 mask 255.255.0.0
      IP Ranges from 10.2.0.0 to 10.2.0.255
Pool name: 2
  Network: 20.1.1.0 mask 255.255.255.0
    IP ranges from 20.1.1.0 to 20.1.1.255
Table 5 Command output
Pool name
Name of the address pool.
Network
Assignable network.
IP ranges
Assignable IP address range.
Secondary networks
Assignable secondary networks.
address range
dhcp server ip-pool
network
Use display dhcp server ip-in-use to display binding information about assigned IP addresses.
display dhcp server ip-in-use [ [ dp-address ip-address | ip ip-address | subnet network-address mask-length | vxlan vxlan-id ] [ vpn-instance vpn-instance-name ] | pool pool-name ]
ip ip-address: Displays binding information about the specified assigned IP address. If you do not specify an IP address, this command displays binding information about all assigned IP addresses.
subnet network-address mask-length: Specifies a subnet by the network address and subnet mask length.
pool pool-name: Displays binding information about assigned IP addresses in the specified address pool. The pool name is a case-insensitive string of 1 to 63 characters.
The binding information can be used by other security modules only when the DHCP server is configured on the gateway of DHCP clients.
If the lease deadline exceeds the year 2100, the lease expiration time is displayed as After 2100.
If you do not specify any parameters, this command displays binding information about all assigned IP addresses.
# Display binding information about all assigned DHCP addresses.
<Sysname> display dhcp server ip-in-use
IP address       Client identifier/    Lease expiration      Type
                 Hardware address
10.1.1.1         4444-4444-4444        Not used              Static(F)
10.1.1.2         0030-3030-2e30-3030-  May 1 14:02:49 2015   Auto(C)
                 662e-3030-3033-2d45-
                 7468-6572-6e65-74
10.1.1.3         0133-3037-392e-3933-  May 1 14:18:22 2016   Auto(C)
                 3037-2e39-3030-32
10.1.1.4         1111-1111-1111        After 2100            Static(C)
Table 6 Command output
IP address
IP address assigned.
Client identifier/Hardware address
Client ID or hardware address. Client ID is specified as a string of hexadecimal numbers, in which the first two characters represents the hardware type value.
·     If an ASCII string is used, the hardware type value is 00, which means no type.
·     If the hardware type is Ethernet, the type value is 01.
·     If the hardware type is token ring, the type value is 06.
Lease expiration
Lease expiration time:
·     Exact time (May 1 14:02:49 2015 in this example)—Time when the lease will expire.
·     Not used—The IP address of the static binding has not been assigned to the specific client.
·     Unlimited—Infinite lease expiration time.
·     After 2100—The lease will expire after 2100.
Binding types:
·     Static(F)—A free static binding whose IP address has not been assigned.
·     Static(O)—An offered static binding whose IP address has been selected and sent by the DHCP server in a DHCP-OFFER packet to the client. Static(C)—A committed static binding whose IP address has been assigned to the DHCP client.
·     Auto(O)—An offered dynamic binding whose IP address has been dynamically selected by the DHCP server and sent in a DHCP-OFFER packet to the DHCP client.
·     Auto(C)—A committed dynamic binding whose IP address has been dynamically assigned to the DHCP client.
Use display dhcp server pool to display information about a DHCP address pool.
display dhcp server pool [ pool-name | vpn-instance vpn-instance-name ] [ subnet-alloc ]
pool-name: Displays information about the specified address pool. The pool name is a case-insensitive string of 1 to 63 characters. If you do not specify the pool-name argument, this command displays information about all address pools.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays information about address pools for the public network.
subnet-alloc: Supports dynamic subnet allocation. If you do not specify this keyword, the command displays information about DHCP address pools that do not support dynamic subnet allocation.
# Display information about all DHCP address pools.
<Sysname> display dhcp server pool
Pool name: 0
  Network 20.1.1.0 mask 255.255.255.0
  class a range 20.1.1.50 20.1.1.60
  bootfile-name abc.cfg
  dns-list 20.1.1.66 20.1.1.67 20.1.1.68
  domain-name www.aabbcc.com
  bims-server ip 192.168.0.51 sharekey cipher $c$3$K13OmQPi791YvQoF2Gs1E+65LOU=
  option 2 ip-address 1.1.1.1
  expired day 1 hour 2 minute 3 second 0
  reserve expired-ip mode client-id time 4294967295 limit 256000
Pool name: 1
  secondary networks:
    20.1.2.0 mask 255.255.255.0
    20.1.3.0 mask 255.255.255.0
  bims-server ip 192.168.0.51 port 50 sharekey cipher $c$3$K13OmQPi791YvQoF2Gs1E+65LOU=
  forbidden-ip 20.1.1.22 20.1.1.36 20.1.1.37
  forbidden-ip 20.1.1.22 20.1.1.23 20.1.1.24
  gateway-list 1.1.1.1 2.2.2.2 4.4.4.4
  nbns-list 5.5.5.5 6.6.6.6 7.7.7.7
  netbios-type m-node
  expired day 1 hour 0 minute 0 second 0 allow-hint
  reserve expired-ip disable
Pool name: 2
  address range 20.1.1.1 to 20.1.1.15
  class departmentA range 20.1.1.20 to 20.1.1.29
  class departmentB range 20.1.1.30 to 20.1.1.40
  next-server 20.1.1.33
  tftp-server domain-name www.dian.org.cn
  tftp-server ip-address 192.168.0.120
  voice-config ncp-ip 10.1.1.2
  voice-config as-ip 10.1.1.5
  voice-config voice-vlan 3 enable
  voice-config fail-over 10.1.1.1 123*
  option 2 ip-address 1.1.1.3
  reserve expired-ip mode mac time 100 limit 100
Pool name: 3
  static bindings:
    ip-address 10.10.1.2 mask 255.0.0.0
      hardware-address 00e0-00fc-0001 ethernet
    ip-address 10.10.1.3 mask 255.0.0.0
      client-identifier aaaa-bbbb
  expired unlimited
# Display information about all DHCP address pools that support dynamic subnet allocation.
<Sysname> display dhcp server pool subnet-alloc
Pool name: pool1
  Network 10.1.1.0 mask 255.255.0.0
  subnet mask-length: 24
  subnet idle-time: 30
  subnet alloc-mode: dp-address
  dns-list 10.1.1.66 10.1.1.67 10.1.1.68
  sub-networks:
    VXLAN: 01 DP_ADDR: 1.1.1.1  10.0.1.0/24 Leased: 1 Expired: 0 Free: 254
    VXLAN: 02 DP_ADDR: 2.2.2.2  10.0.2.0/24 Leased: 1 Expired: 0 Free: 254
Table 7 Command output
Pool name
Name of an address pool.
Network
Assignable network.
subnet mask-length
Mask length of dynamically allocated subnets.
subnet idle-time
Delay time for the DHCP server to reclaim idle subnets.
Advertising dynamically allocated subnets is disabled. This field is not displayed if subnet advertising is enabled.
subnet alloc-mode
Dynamic subnet allocation modes:
·     dp-address—Subnets are allocated based on the DP address of the VXLAN tunnel.
·     vxlan-id—Subnets are allocated based on the VXLAN ID of the access user.
secondary networks
address range
Assignable address range.
DHCP user class and its address range.
static bindings
Static IP-to-MAC/client ID bindings.
option
Customized DHCP option.
expired
Lease duration. If the DHCP server is allowed to use the DHCP client-suggested lease duration, allow-hint is displayed after the lease duration.
remote server
DHCP server address for a DHCP address pool on the DHCP relay agent. If you create a DHCP address pool on the DHCP relay agent and execute the remote-server command, this field is displayed.
active remote server
Active DHCP server address. If you create a DHCP address pool on the DHCP relay agent and execute the remote-server command, this field is displayed. The displayed value depends on the DHCP server selecting algorithm configuration.
·     If the polling algorithm is used, this field displays all. The DHCP relay agent forwards DHCP requests to all DHCP servers.
·     If the master-backup algorithm is used, this field displays the IP address of the active DHCP server. The DHCP relay agent forwards DHCP requests to the master DHCP server first.
bootfile-name
Boot file name.
dns-list
DNS server IP address.
domain-name
Domain name suffix.
bims-server
BIMS server information.
forbidden-ip
IP addresses excluded from dynamic allocation.
gateway-list
Gateway addresses.
nbns-list
WINS server addresses.
netbios-type
NetBIOS node type.
next-server
Next server IP address.
TFTP server name.
TFTP server address.
voice-config ncp-ip
Primary network calling processor address.
voice-config as-ip
Backup network calling processor address.
Voice VLAN.
Failover route.
IP address reservation is enabled in the DHCP address pool.
IP address reservation is disabled in the DHCP address pool.
Information about the reservation mode, reservation time, and the maximum number of expired IP addresses that can be reserved in the DHCP address pool.
VXLAN
ID of the VXLAN where the DHCP client resides.
DP_ADDR
IP address of the DP at the end of the VXLAN tunnel.
Leased
Number of allocated subnets.
Expired
Number of expired allocated subnets.
Free
Number of idle allocated subnets.
Use display dhcp server statistics to display the DHCP server statistics.
pool pool-name: Specifies an address pool by its name, a case-insensitive string of 1 to 63 characters. If you do not specify this option, this command displays information about all address pools.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays DHCP server statistics for the public network.
# Display the DHCP server statistics.
<Sysname> display dhcp server statistics
    Pool number:                       1
    Pool utilization:                  0.39%
    Bindings:
      Automatic:                       1
      Manual:                          0
      Expired:                         0
    Conflict:                          1
    Messages received:                10
      DHCPDISCOVER:                    5
      DHCPREQUEST:                     3
      DHCPDECLINE:                     0
      DHCPRELEASE:                     2
      DHCPINFORM:                      0
      BOOTPREQUEST:                    0
    Messages sent:                     6
      DHCPOFFER:                       3
      DHCPACK:                         3
      DHCPNAK:                         0
      BOOTPREPLY:                      0
    Bad Messages:                      0
Table 8 Command output
Pool number
Total number of address pools. This field is not displayed when you display statistics for a specific address pool.
Pool utilization
Pool usage rate:
·     If you display statistics for all address pools, this field displays the usage rate of all address pools.
·     If you display statistics for an address pool, this field displays the pool usage rate of the specified address pool.
Bindings
Bindings include the following types:
·     Automatic—Number of dynamic bindings.
·     Manual—Number of static bindings.
·     Expired—Number of expired bindings.
Conflict
Total number of conflict addresses. This field is not displayed if you display statistics for a specific address pool.
Messages received
DHCP packets received from clients:
·     DHCPDISCOVER.
·     DHCPREQUEST.
·     DHCPDECLINE.
·     DHCPRELEASE.
·     DHCPINFORM.
·     BOOTPREQUEST.
Messages sent
DHCP packets sent to clients:
·     DHCPOFFER.
·     DHCPACK.
·     DHCPNAK.
·     BOOTPREPLY.
This field is not displayed if statistics about a specific address pool are displayed.
Bad Messages
Number of bad messages. This field is not displayed if you display statistics for a specific address pool.
dns-list
Use dns-list to specify DNS server addresses in a DHCP address pool.
Use undo dns-list to remove DNS server addresses from a DHCP address pool.
dns-list ip-address&<1-8>
undo dns-list [ ip-address&<1-8> ]
No DNS server address is specified.
ip-address&<1-8>: Specifies a space-separated list of up to eight DNS servers.
If you do not specify any parameters, the undo dns-list command deletes all DNS server addresses in the DHCP address pool.
# Specify DNS server address 10.1.1.254 in DHCP address pool 0.
[Sysname-dhcp-pool-0] dns-list 10.1.1.254
domain-name
Use domain-name to specify a domain name in a DHCP address pool.
Use undo domain-name to restore the default.
domain-name domain-name
undo domain-name
No domain name is specified.
domain-name: Specifies the domain name, a case-sensitive string of 1 to 50 characters.
# Specify domain name company.com in DHCP address pool 0.
[Sysname-dhcp-pool-0] domain-name company.com
expired
Use expired to set the lease duration in a DHCP address pool.
Use undo expired to restore the default lease duration for a DHCP address pool.
expired { allow-hint | { day day [ hour hour [ minute minute [ second second ] ] ] | unlimited } [ allow-hint ] }
undo expired
The lease duration of a dynamic DHCP address pool is one day.
allow-hint: Allows the DHCP server to use the DHCP client-suggested lease duration. The DHCP server uses the DHCP client-suggested lease duration if the DHCP client-suggested lease duration is shorter than the lease duration in the DHCP address pool. If you do not specify this keyword, the DHCP server always uses the lease duration in the DHCP address pool.
day day: Specifies the number of days, in the range of 0 to 365.
hour hour: Specifies the number of hours, in the range of 0 to 23. The default is 0.
minute minute: Specifies the number of minutes, in the range of 0 to 59. The default is 0.
second second: Specifies the number of seconds, in the range of 0 to 59. The default is 0.
unlimited: Specifies the unlimited lease duration, which is actually 136 years.
The DHCP server assigns an IP address together with the lease duration to the DHCP client. Before the lease expires, the DHCP client must extend the lease duration.
·     If the lease extension operation succeeds, the DHCP client can continue to use the IP address.
·     If the lease extension operation does not succeed, both of the following events occur:
¡     The DHCP client cannot use the IP address after the lease duration expires.
¡     The DHCP server will label the IP address as expired.
# Set the lease duration to 1 day, 2 hours, 3 minutes, and 4 seconds in DHCP address pool 0.
[Sysname-dhcp-pool-0] expired day 1 hour 2 minute 3 second 4
# Set the lease duration to 1 day, 2 hours, 3 minutes, and 4 seconds in DHCP address pool 0. Allow the DHCP server to use the DHCP client-suggested lease duration.
[Sysname-dhcp-pool-0] expired day 1 hour 2 minute 3 second 4 allow-hint
forbidden-ip
Use forbidden-ip to exclude IP addresses from dynamic allocation in an address pool.
Use undo forbidden-ip to remove the configuration.
forbidden-ip ip-address&<1-8>
undo forbidden-ip [ ip-address&<1-8> ]
No IP addresses are excluded from dynamic allocation in an address pool.
ip-address&<1-8>: Specifies a space-separated list of up to eight excluded IP addresses.
The excluded IP addresses in an address pool are still assignable in other address pools.
You can exclude a maximum of 4096 IP addresses in an address pool by executing this command multiple times.
If you do not specify any parameters, the undo forbidden-ip command removes all excluded IP addresses.
# Exclude IP addresses 192.168.1.3 and 192.168.1.10 from dynamic allocation in DHCP address pool 0.
[Sysname-dhcp-pool-0] forbidden-ip 192.168.1.3 192.168.1.10
forbidden-ip-range
Use forbidden-ip-range to exclude an IP address range from DHCP allocation in an address pool.
Use undo forbidden-ip-range to remove an IP address range from the forbidden IP range list.
forbidden-ip-range start-ip-address [ end-ip-address ]
undo forbidden-ip-range [ start-ip-address [ end-ip-address ] ]
No IP address ranges are excluded from DHCP allocation in an address pool.
IP address pool view
start-ip-address: Specifies a start IP address.
end-ip-address: Specifies an end IP address. The end IP address cannot be lower than the start IP address. If you do not specify this argument, the excluded IP range includes only the start IP address.
The forbidden IP ranges in an address pool are still assignable in other address pools.
To specify multiple forbidden IP ranges, execute the forbidden-ip-range command multiple times. The forbidden IP ranges can overlap.
When you execute the undo form of this command to remove forbidden IP ranges, follow these guidelines:
·     To remove all forbidden IP ranges, execute the undo forbidden-ip-range command without specifying any parameters.
·     To remove a subrange of IP addresses from a forbidden IP range, specify only that subrange of IP addresses.
·     To remove a forbidden IP range as a whole, specify that IP range or an IP range broader than it.
# Exclude IP address range from 192.168.1.3 to 192.168.1.10 from DHCP allocation in IP address pool pool1.
[Sysname-dhcp-pool-pool1] forbidden-ip-range 192.168.1.3 192.168.1.10
gateway-list
Use gateway-list to specify gateway addresses in a DHCP address pool or a DHCP secondary subnet.
Use undo gateway-list to remove the specified gateway addresses from a DHCP address pool or a DHCP secondary subnet.
gateway-list ip-address&<1-64> [ export-route ]
undo gateway-list [ ip-address&<1-64> ] [ export-route ]
No gateway address is configured in a DHCP address pool or a DHCP secondary subnet.
DHCP secondary subnet view
ip-address&<1-64>: Specifies a space-separated list of up to 64 gateway addresses. Gateway addresses must reside on the same subnet as the assignable IP addresses.
export-route: Binds the gateways to the device's MAC address in the address management module. The ARP module will use the entries to reply to ARP requests from the DHCP clients. If you do not specify this keyword, the gateways will not be bound to the device's MAC address.
The DHCP server assigns gateway addresses to clients on a secondary subnet in the following ways:
·     If gateways are specified in both address pool view and secondary subnet view, DHCP assigns those specified in the secondary subnet view.
·     If gateways are specified in address pool view but not in secondary subnet view, DHCP assigns those specified in address pool view.
If you do not specify any parameters, the undo gateway-list command deletes all gateway addresses.
# Specify gateway address 10.1.1.1 in DHCP address pool 0.
[Sysname-dhcp-pool-0] gateway-list 10.1.1.1
if-match
Use if-match to configure a match rule for a DHCP user class.
Use undo if-match to delete a match rule for a DHCP user class.
No match rules are configured for the DHCP user class.
rule rule-number: Assigns the match rule an ID in the range of 1 to 16. A smaller ID represents a higher match priority.
hardware-address hardware-address: Specifies a hardware address, a string of 4 to 39 characters. The string contains hyphen-separated hexadecimal numbers. The last hexadecimal number can be a two-digit or four-digit number, and the other hexadecimal numbers must be four-digit numbers. For example, aabb-ccdd-ee is valid, and aabb-c-dddd or aabb-cc-dddd is invalid.
mask hardware-address-mask: Specifies the mask to be ANDed with the specified hardware address for the match operation. The length of the mask must be the same as that of the hardware address.
option option-code: Specifies a DHCP option by its number in the range of 1 to 254.
ascii ascii-string: Specifies an ASCII string of 1 to 128 characters.
offset offset: Specifies the offset in bytes after which the match operation starts. The value range is 0 to 254. If you do not specify an offset value, the match starts from the first byte of the option content. If you specify an ASCII string, a packet matches the rule if the option content after the offset is the same as the ASCII string. If you specify a hexadecimal number, a packet matches the rule if the option content of the specified length after the offset is the same as the hexadecimal number.
partial: Enables partial match. A packet matches a rule if the specified option in the packet contains the ASCII string or hexadecimal number specified in the rule. For example, if you specify abc in the rule, option content xabc, xyzabca, xabcyz, and abcxyz all match the rule.
hex hex-string: Specifies a hexadecimal number. The length of the hexadecimal number must be an even number in the range of 2 to 256.
mask mask: Specifies a hexadecimal mask for the match operation. The mask length must be an even number in the range of 2 to 256 and be the same as the hex-string length. The DHCP server selects option content of the mask length from the start and ANDs the selected option content and the specified hexadecimal number with the mask. The packet matches the rule if the two AND operation results are the same.
length length: Specifies the length of the option content to be matched, in the range of 1 to 128 bytes. The length must be the same as the hex-string length.
relay-agent gateway-address: Specifies a giaddr field value. The value is an IPv4 address in the dotted decimal notation. A packet matches the rule if its giaddr field value is the same as that in the rule.
If a DHCP request sent by a DHCP client matches a rule in a DHCP user class, the DHCP client matches the user class.
You can configure multiple match rules for a DHCP user class. Each match rule is uniquely identified by a rule ID within its type (hardware address, option, or relay agent address).
·     If the rule that you are configuring has the same ID and type as an existing rule, the new rule overwrites the existing rule.
·     If the rule that you are configuring has the same ID as an existing rule but a different type, the new rule takes effect and coexists with the existing rule. As a best practice, do not assign the same ID to rules of different types.
·     Rules of different IDs cannot have the same rule content.
When you configure an if-match hardware-address rule, follow these guidelines:
·     The hardware address type supports only the MAC address. A rule does not match clients with hardware addresses of other types.
·     The specified hardware address must be of the same length as the client hardware addresses to be matched. To match MAC addresses, the specified hardware address must be six bytes long.
·     The fs and 0s in the mask for the hardware match operation can be noncontiguous. For example, the rule if-match rule 1 hardware-address 0094-0000-1100 mask ffff-0000-ff00 matches hardware addresses in which the first two bytes are 0094 and the fifth byte is 11.
When you configure an if-match option rule, follow these guidelines:
·     To match packets that contain an option, specify only the option-code argument.
·     To match a hexadecimal number by AND operations, specify the option option-code hex hex-string mask mask options.
·     To match a hexadecimal number directly, specify the option option-code hex hex-string [ offset offset length length | partial ] options. If you do not specify the offset, length, or partial parameter, a packet matches a rule if the option content starts with the hexadecimal number.
·     To match an ASCII string, specify the option option-code ascii ascii-string [ offset offset | partial ] options. If you do not specify the offset or partial parameter, a packet matches a rule if the option content starts with the ASCII string.
# Configure match rule 1 for DHCP user class exam to match DHCP requests in which the hardware address is six bytes long and begins with 0094.
[Sysname] dhcp class exam
[Sysname-dhcp-class-exam] if-match rule 1 hardware-address 0094-0000-0101 mask ffff-0000-0000
# Configure match rule 2 for DHCP user class exam to match DHCP requests that contain Option 82.
[Sysname-dhcp-class-exam] if-match rule 2 option 82
# Configure match rule 3 for DHCP user class exam. The rule matches DHCP requests in which the highest bit of the fourth byte in Option 82 is the hexadecimal number 1.
[Sysname-dhcp-class-exam] if-match rule 3 option 82 hex 00000080 mask 00000080
# Configure match rule 4 for DHCP user class exam. The rule matches DHCP requests in which the first three bytes of Option 82 are the hexadecimal number 13ae92.
[Sysname-dhcp-class-exam] if-match rule 4 option 82 hex 13ae92 offset 0 length 3
# Configure match rule 5 for DHCP user class exam. The rule matches DHCP requests in which the Option 82 contains the hexadecimal number 13ae.
[Sysname-dhcp-class-exam] if-match rule 5 option 82 hex 13ae partial
# Configure match rule 6 for DHCP user class exam to match DHCP requests in which the giaddr field is 10.1.1.1.
[Sysname-dhcp-class-exam] if-match rule 6 relay-agent 10.1.1.1
dhcp class
ip-in-use threshold
Use ip-in-use threshold to set the DHCP address pool usage threshold.
Use undo ip-in-use threshold to restore the default.
The DHCP address pool usage threshold is 100%.
DHCP address pool view
threshold-value: Specifies the usage threshold in percentage in the range of 0 to 100.
If the usage of a DHCP address pool exceeds the threshold, the DHCP module sends an SNMP notification and a log message to report the event. You can optimize the DHCP address pool configuration accordingly. If the threshold value is set to 100%, the DHCP module generates only an SNMP notification when the IP pool usage reaches 100% or drops below 90%.
For DHCP notifications to be sent correctly, you must configure SNMP on the device. For log messages to be sent correctly, you must configure the information center. For more information about SNMP configuration, see Network Management and Monitoring Configuration Guide. For more information about the information center configuration, see System Management Configuration Guide.
If you execute this command multiple times in the same DHCP address pool view, the most recent configuration takes effect.
# Set the DHCP address pool usage threshold to 85%.
[Sysname] dhcp server ip-pool p1
[Sysname-dhcp-pool-p1] ip-in-use threshold 85
snmp-agent trap enable dhcp server
nbns-list
Use nbns-list to specify WINS server addresses in a DHCP address pool.
Use undo nbns-list to remove the specified WINS server addresses.
nbns-list ip-address&<1-8>
undo nbns-list [ ip-address&<1-8> ]
No WINS server address is specified.
ip-address&<1-8>: Specifies a space-separated list of up to eight WINS server IP addresses.
If you do not specify any parameters, the undo nbns-list command deletes all WINS server addresses.
# Specify WINS server address 10.1.1.1 in DHCP address pool 0.
[Sysname] dhcp server ip-pool 0
[Sysname-dhcp-pool-0] nbns-list 10.1.1.1
netbios-type
netbios-type
Use netbios-type to specify the NetBIOS node type in a DHCP address pool.
Use undo netbios-type to restore the default.
undo netbios-type
No NetBIOS node type is specified.
b-node: Specifies the broadcast node. A b-node client sends the destination name in a broadcast message to get the name-to-IP mapping from a server.
h-node: Specifies the hybrid node. An h-node client unicasts the destination name to a WINS server. If it does not receive a response, the h-node client broadcasts the destination name to get the mapping from a server.
m-node: Specifies the mixed node. An m-node client broadcasts the destination name. If it does not receive a response, the m-node client unicasts the destination name to the WINS server to get the mapping.
p-node: Specifies the peer-to-peer node. A p-node client sends the destination name in a unicast message to get the mapping from the WINS server.
# Specify the NetBIOS node type as p-node in DHCP address pool 0.
[Sysname-dhcp-pool-0] netbios-type p-node
nbns-list
network
Use network to specify the subnet for dynamic allocation in a DHCP address pool.
Use undo network to remove the specified subnet.
network network-address [ mask-length | mask mask ] [ export-route [ preference preference | tag tag ] * ] [ secondary ]
undo network network-address [ mask-length | mask mask ] [ secondary ]
No subnet is specified in a DHCP address pool.
network-address: Specifies the subnet for dynamic allocation. If no mask length or mask is specified, the natural mask will be used.
mask-length: Specifies the mask length in the range of 1 to 30.
mask mask: Specifies the mask in dotted decimal format.
export-route: Advertises the subnet assigned to DHCP clients. If you do not specify this keyword, the subnet will not be advertised.
preference preference: Sets a preference for the network route to be advertised, in the range of 1 to 255. The default preference is 70.
tag tag: Sets a tag value for the network route to be advertised, in the range of 0 to 4294967295. The default tag value is 0. Tags are route identifications for routing policies to filter routes. For more information about routing policies, see Layer 3—IP Routing Configuration Guide.
secondary: Specifies the subnet as a secondary subnet. If you do not specify this keyword, this command specifies the primary subnet. If the addresses in the primary subnet are used up, the DHCP server can select addresses from a secondary subnet for clients.
You can use the secondary keyword to specify a secondary subnet and enter its view. In secondary subnet view, you can specify gateways by using the gateway-list command for DHCP clients in the secondary subnet.
You can specify only one primary subnet for a DHCP address pool. If you execute the network command multiple times, the most recent configuration takes effect.
You can specify up to 32 secondary subnets for a DHCP address pool.
The primary subnet and secondary subnets in a DHCP address pool must not have the same network address and mask.
If you have used the address range or class command in an address pool, you cannot specify a secondary subnet in the same address pool.
Modifying or removing the network configuration deletes the assigned addresses from the current address pool.
If you execute the network export-route command multiple times, the most recent configuration takes effect.
# Specify primary subnet 192.168.8.0/24 and secondary subnet 192.168.10.0/24 in DHCP address pool 0.
[Sysname-dhcp-pool-0] network 192.168.8.0 mask 255.255.255.0
[Sysname-dhcp-pool-0] network 192.168.10.0 mask 255.255.255.0 secondary
[Sysname-dhcp-pool-0-secondary]
gateway-list
subnet alloc-mode
·     subnet export-route disable
subnet idle-time
·     subnet mask-length
next-server
Use next-server to specify the IP address of a server in a DHCP address pool.
Use undo next-server to restore the default.
next-server ip-address
undo next-server
No server's IP address is specified in a DHCP address pool.
ip-address: Specifies the IP address of a server.
Upon startup, the DHCP client obtains an IP address and the specified server IP address. Then it contacts the specified server, such as a TFTP server, to get other boot information.
# Specify a server's IP address 10.1.1.254 in DHCP address pool 0.
[Sysname-dhcp-pool-0] next-server 10.1.1.254
option
Use option to customize a DHCP option.
Use undo option to remove a customized DHCP option.
undo option code
No DHCP option is customized.
code: Specifies the number of the customized option, in the range of 2 to 254, excluding 50 through 54, 56, 58, 59, 61, and 82.
ascii ascii-string: Specifies a case-sensitive ASCII string of 1 to 255 characters as the option content.
hex hex-string: Specifies a hexadecimal number as the option content. The length of the hexadecimal number must be an even number in the range of 2 to 256.
ip-address ip-address&<1-8>: Specifies a space-separated list of up to eight IP addresses as the option content.
The DHCP server fills the customized option with the specified ASCII string, hexadecimal number, or IP addresses, and sends it in a response to the client.
You can customize options for the following purposes:
·     Add newly released options.
·     Add options for which the vendor defines the contents, for example, Option 43.
·     Add options for which the CLI does not provide a dedicated configuration command. For example, you can use the option 4 ip-address 1.1.1.1 command to define the time server address 1.1.1.1 for DHCP clients.
·     Add all option values if the actual requirement exceeds the limit for a dedicated option configuration command. For example, the dns-list command can specify up to eight DNS servers. To specify more than eight DNS server, you must use the option 6 command to define all DNS servers.
DHCP options specified by dedicated commands take precedence over those specified by the option commands. For example, if a DNS server address is specified by both the dns-list command and the option 6 command, the server uses the address specified by the dns-list command.
DHCP options specified in DHCP option groups take precedence over those specified in DHCP address pools.
If multiple DHCP option groups have the same option, the server selects the option in the DHCP option group first matching the user class.
If you execute this command multiple times with the same code specified, the most recent configuration takes effect.
# Configure Option 7 to specify log server address 2.2.2.2 in DHCP address pool 0.
[Sysname-dhcp-pool-0] option 7 ip-address 2.2.2.2
Use reserve expired-ip enable to enable IP address reservation in a DHCP address pool.
Use undo reserve expired-ip enable to disable IP address reservation in a DHCP address pool.
IP address reservation is enabled.
This feature enables the DHCP server to reserve IP addresses for clients that are going offline. When a client goes offline, the DHCP server reserves the client IP address as an expired lease. When the client comes online again, the DHCP server assigns the IP address in the reserved lease to the client.
Disable the IP address reservation feature if you want the DHCP server to reclaim IP addresses immediately after clients go offline.
# Disable IP address reservation in DHCP address pool 0.
[Sysname-dhcp-pool-0] undo reserve expired-ip enable
Use reserve expired-ip enable to configure the IP address reservation mode in a DHCP address pool.
Use undo reserve expired-ip enable to restore the default.
reserve expired-ip mode { client-id | mac } [ limit limit-number | time time ] *
undo reserve expired-ip mode
With IP address reservation enabled, a DHCP server reserves IP addresses based on client IDs.
client-id: Reserves IP addresses based on client IDs.
Mac: Reserves IP addresses based on client MAC addresses.
limit limit-number: Specifies the maximum number of IP addresses that can be reserved in a DHCP address pool. The value range is 1 to 256000, and the default value is 256000.
time time: Specifies the reservation time for expired IP addresses, in the range of 60 to 4294967295 seconds. If you do not specify this option, the reserved time is unlimited (about 136 years defined by the system).
With IP address reservation enabled, the DHCP server reserves IP addresses for DHCP clients in the following modes:
·     Reservation based on client IDs—The DHCP server records the IP-to-client ID bindings for online clients. When these clients come online again, the server assigns them the IP addresses in the bindings based on their client IDs.
·     Reservation based on client MAC addresses—The DHCP server records the IP-to-MAC bindings for online clients. When these clients come online again, the server assigns them the IP addresses in the bindings based on their MAC addresses.
When you change the IP address reservation mode, the device deletes all expired leases that are saved in the old reservation mode.
# Configure the DHCP server to reserve IP addresses based on client IDs in DHCP address pool 0.
[Sysname-dhcp-pool-0] reserve expired-ip enable
[Sysname-dhcp-pool-0] reserve expired-ip mode client-id
reset dhcp server conflict
Use reset dhcp server conflict to clear IP address conflict information.
ip ip-address: Clears conflict information about the specified IP address. If you do not specify this option, this command clears all address conflict information.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears conflict information about IP addresses for the public network.
Address conflicts occur when dynamically assigned IP addresses have been statically configured for other hosts. After you modify the address pool configuration, the conflicted addresses might become assignable. To assign these addresses, use the reset dhcp server conflict command to clear the conflict information first.
# Clear all IP address conflict information.
<Sysname> reset dhcp server conflict
reset dhcp server expired
Use reset dhcp server expired to clear binding information about expired IP addresses.
reset dhcp server expired [ [ ip ip-address ] [ vpn-instance vpn-instance-name ] | pool pool-name ]
ip ip-address: Clears binding information about the specified expired IP address. If you do not specify an IP address, this command clears binding information about all expired IP addresses.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears lease expiration information about IP addresses for the public network.
pool pool-name: Clears binding information about the expired IP addresses in the specified address pool. The pool name is a case-insensitive string of 1 to 63 characters. If you do not specify an address pool, this command clears binding information about expired IP addresses in all address pools.
# Clear binding information about all expired IP addresses.
<Sysname> reset dhcp server expired
reset dhcp server ip-in-use
Use reset dhcp server ip-in-use to clear binding information about assigned IP addresses.
ip ip-address: Clears binding information about the specified assigned IP address. If you do not specify an IP address, this command clears binding information about all assigned IP addresses.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears binding information for the public network.
pool pool-name: Clears binding information about assigned IP addresses in the specified address pool. The pool name is a case-insensitive string of 1 to 63 characters. If you do not specify an address pool, this command clears binding information about assigned IP addresses in all address pools.
If you use this command to clear information about an assigned static binding, the static binding becomes a free static binding.
# Clear binding information about IP address 10.110.1.1.
<Sysname> reset dhcp server ip-in-use ip 10.110.1.1
reset dhcp server statistics
Use reset dhcp server statistics to clear DHCP server statistics.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears DHCP server statistics for the public network.
# Clear DHCP server statistics.
<Sysname> reset dhcp server statistics
Use snmp-agent trap enable dhcp server to enable SNMP notifications for the DHCP server.
Use undo snmp-agent trap enable dhcp server to disable SNMP notifications for the DHCP server.
snmp-agent trap enable dhcp server [ address-exhaust | allocated-ip | ip-in-use ]
SNMP notifications are enabled for the DHCP server.
address-exhaust: Specifies notifications about the exhaustion or recovery of a DHCP address pool.
allocated-ip: Specifies notifications about IP address allocation success rate threshold violation. The threshold is set by the dhcp server allocated-ip threshold command.
ip-in-use: Specifies notifications about the usage threshold violation in a DHCP address pool. The threshold is set by the ip-in-use threshold command.
If you do not specify any parameters, this command enables SNMP notifications for all types of DHCP server events.
To report critical DHCP server events to an NMS, enable SNMP notifications for the DHCP server. For DHCP server event notifications to be sent correctly, you must also configure SNMP on the device. For more information about SNMP configuration, see the network management and monitoring configuration guide for the device.
# Enable SNMP notifications for all types of DHCP server events.
[Sysname] snmp-agent trap enable dhcp server
# Enable SNMP notifications for DHCP address pool exhaustion or recovery.
[Sysname] snmp-agent trap enable dhcp server address-exhaust
# Enable SNMP notifications for IP address allocation success rate threshold violation.
[Sysname] snmp-agent trap enable dhcp server allocated-ip
# Enable SNMP notifications for DHCP address pool usage threshold violation.
[Sysname] snmp-agent trap enable dhcp server ip-in-use
ip-in-use threshold
snmp-agent target-host (Network Management and Monitoring Command Reference)
static-bind
Use static-bind to statically bind a client ID or MAC address to an IP address.
Use undo static-bind to remove a static binding.
undo static-bind ip-address ip-address
No static binding is specified in a DHCP address pool.
ip-address ip-address: Specifies the IP address of the static binding. The natural mask is used if no mask length or mask is specified.
mask mask: Specifies the mask, in dotted decimal format.
client-identifier client-identifier: Specifies the client ID of the static binding, a string of 4 to 254 characters. The string can contain only hexadecimal numbers and hyphen (-), in the format of H-H-H…. The last H can be a two-digit or four-digit hexadecimal number while the other Hs must be all four-digit hexadecimal numbers. For example, aabb-cccc-dd is correct, and aabb-c-dddd and aabb-cc-dddd are not correct.
hardware-address hardware-address: Specifies the client hardware address of the static binding, a string of 4 to 39 characters. The string can contain only hexadecimal numbers and hyphen (-), in the format of H-H-H…. The last H can be a two-digit or four-digit hexadecimal number while the other Hs must be all four-digit hexadecimal numbers. For example, aabb-cccc-dd is correct, and aabb-c-dddd and aabb-cc-dddd are not correct.
ethernet: Specifies the client hardware address type as Ethernet. The default type is Ethernet.
token-ring: Specifies the client hardware address type as token ring.
The IP address of a static binding must not be an interface address of the DHCP server. Otherwise, an IP address conflict occurs, and the bound client cannot obtain the IP address.
You can repeat this command to specify multiple static bindings in an address pool.
An IP address can be bound to only one DHCP client. To modify the binding for a DHCP client, first execute the undo form of the command to delete the existing binding and then create a new binding.
# Bind IP address 10.1.1.1/24 to client ID 00aa-aabb in DHCP address pool 0.
[Sysname-dhcp-pool-0] static-bind ip-address 10.1.1.1 mask 255.255.255.0 client-identifier 00aa-aabb
subnet alloc-mode
Use subnet alloc-mode to specify a subnet allocation mode for a DHCP address pool that supports dynamic subnet allocation.
Use undo subnet alloc-mode to restore the default.
subnet alloc-mode { dp-address | vxlan-id }
Subnets are allocated based on VXLAN IDs in the DHCP address pool that supports dynamic subnet allocation.
dp-address: Allocates a subnet to a DP based on the DP address of the VXLAN tunnel.
vxlan-id: Allocates a subnet to a DP based on the VXLAN ID of the user on the DP.
When the users connecting to a DP are of different types or at different locations, configure the address allocation based on the VXLAN IDs of the users. In other situations, configure the address allocation based on the DP address of the VXLAN tunnel.
The subnet allocation mode switchover causes the DHCP server to reclaim assigned subnets and perform re-allocation. As a best practice, determine the subnet allocation mode before configuring the DHCP server to allocate subnets.
# Configure the DHCP server to allocate subnet based on the DP address of the VXLAN tunnel.
[Sysname] dhcp server ip-pool pool1 subnet-alloc
[Sysname-dhcp-pool-pool1] subnet alloc-mode dp-address
network
Use subnet export-route disable to disable the DHCP server from issuing routes for an IP address pool that supports dynamic subnet allocation.
Use undo subnet export-route disable to enable the DHCP server to issue routes for an IP address pool that supports dynamic subnet allocation.
The DHCP server issues routes for IP address pools that support dynamic subnet allocation.
In a CUPS scenario, the CP acts as the DHCP server. When the CP and UP are colocated on the same device, only the network route rather than the subnet routes can be advertised to reduce the number of routes. In this case, you can disable the DHCP server from issuing routes for IP address pools that support dynamic subnet allocation. Then, execute the network export-route command to advertise the network route to the UP.
# Disable the DHCP server from issuing routes for an IP address pool that supports dynamic subnet allocation.
[Sysname-dhcp-pool-pool1] subnet export-route disable
network
subnet idle-time
Use subnet idle-time to set the delay time for the DHCP server to reclaim idle subnets.
subnet idle-time time
undo subnet idle-time
The delay time for the DHCP server to reclaim idle subnets is 1 second.
time: Sets the delay time for the DHCP server to reclaim idle subnets in seconds. The value range is 1 to 4294967295.
When all users on a subnet go offline, the CP reclaims the idle subnet. When the users come online again, the CP assigns them IP addresses in another subnet. To avoid assigning IP addresses of different subnets to a user that comes online and goes offline frequently, increase the delay time for the CP to reclaim idle subnets.
# Set the delay time for the CP to reclaim idle subnets to 10 seconds.
[Sysname] subnet idle-time 10
network
subnet mask-length
Use subnet mask-length to specify the mask length for dynamically allocated subnets in a DHCP address pool.
Use undo subnet alloc-mode to remove the configuration.
subnet mask-length mask-len
undo subnet mask-length
No mask length is specified for dynamically allocated subnets in a DHCP address pool.
mask-len: Specifies the subnet mask length in the range of 1 to 30. The subnet mask length must be longer than or equal to the mask length specified in the network command in the DHCP address pool.
After the DHCP server has assigned IP addresses, do not use the subnet mask-length command to modify the mask length. Doing so will release all dynamically allocated subnets in the address pool.
# Create DHCP address pool pool1 that support dynamic subnet allocation and set the mask length to 24 for dynamically allocated subnets.
[Sysname] network 10.1.0.0 16
[Sysname] subnet mask-length 24
network
Use tftp-server domain-name to specify a TFTP server name in a DHCP address pool.
Use undo tftp-server domain-name to restore the default.
No TFTP server name is specified.
domain-name: Specifies the TFTP server name, a case-sensitive string of 1 to 63 characters.
# Specify TFTP server name aaa in DHCP address pool 0.
[Sysname-dhcp-pool-0] tftp-server domain-name aaa
Use tftp-server ip-address to specify a TFTP server address in a DHCP address pool.
Use undo tftp-server ip-address to restore the default.
No TFTP server address is specified.
ip-address: Specifies the IP address of a TFTP server.
# Specify TFTP server address 10.1.1.1 in DHCP address pool 0.
[Sysname-dhcp-pool-0] tftp-server ip-address 10.1.1.1
valid class
Use valid class to add DHCP user classes to the whitelist.
Use undo valid class to remove DHCP user classes from the whitelist.
valid class class-name&<1-8>
undo valid class class-name&<1-8>
No DHCP user class is listed on the whitelist.
class-name&<1-8>: Specifies a space-separated list of up to eight DHCP user classes by their names, a case-insensitive string of 1 to 63 characters.
For this command to take effect, you must enable the DHCP user class whitelist.
# Add DHCP user classes test1 and test2 to the whitelist in DHCP address pool 0.
[Sysname-dhcp-pool-0] valid class test1 test2
dhcp class
verify class
verify class
Use verify class to enable the DHCP user class whitelist.
Use undo verify class to disable the DHCP user class whitelist.
verify class
undo verify class
The DHCP user class whitelist is disabled.
After you enable the DHCP user class whitelist, the DHCP server processes requests only from clients on the DHCP user class whitelist.
The DHCP user class whitelist does not take effect on clients that request static IP addresses, and the server always processes their requests.
# Enable the DHCP user class whitelist in DHCP address pool 0.
[Sysname] system-view
[Sysname-dhcp-pool-0] verify class
valid class
voice-config
Use voice-config to configure the content for Option 184 in a DHCP address pool.
Use undo voice-config to remove the Option 184 content from a DHCP address pool.
voice-config { as-ip ip-address | fail-over ip-address dialer-string | ncp-ip ip-address | voice-vlan vlan-id { disable | enable } }
undo voice-config [ as-ip | fail-over | ncp-ip | voice-vlan ]
No Option 184 content is configured in a DHCP address pool.
as-ip ip-address: Specifies the IP address of the backup network calling processor.
fail-over ip-address dialer-string: Specifies the failover IP address and dialer string. The dialer-string is a string of 1 to 39 characters. Valid characters are digits and asterisk (*).
ncp-ip ip-address: Specifies the IP address of the primary network calling processor.
voice-vlan vlan-id: Specifies the voice VLAN ID in the range of 2 to 4094.
·     disable: Disables the specified VLAN. DHCP clients will not take this VLAN as their voice VLAN.
·     enable: Enables the specified VLAN. DHCP clients will take this VLAN as their voice VLAN.
# Configure Option 184 in DHCP address pool 0. The primary and backup network calling processors are at 10.1.1.1 and 10.2.2.2, respectively. The voice VLAN 3 is enabled. The failover IP address is 10.3.3.3. The dialer string is 99*.
[Sysname-dhcp-pool-0] voice-config ncp-ip 10.1.1.1
[Sysname-dhcp-pool-0] voice-config as-ip 10.2.2.2
[Sysname-dhcp-pool-0] voice-config voice-vlan 3 enable
[Sysname-dhcp-pool-0] voice-config fail-over 10.3.3.3 99*
vpn-instance
Use vpn-instance to apply a DHCP address pool to a VPN instance.
Use undo vpn-instance to restore the default.
undo vpn-instance
The DHCP address pool is not applied to any VPN instance.
If a DHCP address pool is applied to a VPN instance, the DHCP server assigns IP addresses in this address pool to clients in the specified VPN instance.
The DHCP server identifies the VPN instance to which a DHCP client belongs according to the following information:
·     The client's VPN information stored in authentication modules.
·     The VPN information of the DHCP server's interface that receives DHCP packets from the client.
The VPN information from authentication modules takes priority over the VPN information of the receiving interface.
# Apply DHCP address pool 0 to VPN instance abc.
[Sysname-dhcp-pool-0] vpn-instance abc
DHCP relay agent commands
dhcp relay always-unicast
Use dhcp relay always-unicast to enable the DHCP relay agent to always unicast relayed DHCP responses.
Use undo dhcp relay always-unicast to restore the default.
The DHCP relay agent reads the broadcast flag in a DHCP response to decide whether to broadcast or unicast the relayed response.
This command enables the DHCP server to ignore the broadcast flag in DHCP responses and always unicast all relayed responses.
# Enable the DHCP relay agent to always unicast relayed DHCP responses.
[Sysname] dhcp relay always-unicast
dhcp select relay
dhcp relay check mac-address
Use dhcp relay check mac-address to enable MAC address check on the relay agent.
Use undo dhcp relay check mac-address to disable MAC address check on the relay agent.
The MAC address check feature is disabled.
Interface view
This feature enables the DHCP relay agent to compare the chaddr field of a received DHCP request with the source MAC address in the frame header. If they are the same, the DHCP relay agent forwards the request to the DHCP server. If they are not the same, the DHCP relay agent discards the request.
The MAC address check feature takes effect only when the dhcp select relay command has already been configured on the interface.
Enable the MAC address check feature only on the DHCP relay agent directly connected to the DHCP clients. A DHCP relay agent changes the source MAC address of DHCP packets before sending them.
# Enable MAC address check on the DHCP relay agent.
[Sysname] interface gigabitethernet 0/0/1
[Sysname-GigabitEthernet0/0/1] dhcp relay check mac-address
dhcp select relay
dhcp relay check mac-address aging-time
Use dhcp relay check mac-address aging-time to set the aging time for MAC address check entries on the DHCP relay agent.
Use undo dhcp relay check mac-address aging-time to restore the default.
The aging time is 30 seconds.
time: Specifies the aging time for MAC address check entries, in the range of 30 to 600 seconds.
This command takes effect only after you execute the dhcp relay check mac-address command.
# Set the aging time to 60 seconds for MAC address check entries on the DHCP relay agent.
[Sysname] dhcp relay check mac-address aging-time 60
dhcp relay client-information record
Use dhcp relay client-information record to enable recording client information in relay entries.
Use undo dhcp relay client-information record to disable the feature.
The DHCP relay agent does not record client information in relay entries.
Client information is recorded only when the DHCP relay agent is configured on the gateway of DHCP clients. A relay entry contains information about a client such as the client's IP and MAC addresses.
Disabling the recording of client information deletes all recorded relay entries.
# Enable the recording of relay entries on the relay agent.
[Sysname] dhcp relay client-information record
dhcp relay client-information refresh
dhcp relay client-information refresh enable
Use dhcp relay client-information refresh to set the interval at which the DHCP relay agent refreshes relay entries.
Use undo dhcp relay client-information refresh to restore the default.
dhcp relay client-information refresh [ auto | interval interval ]
The refresh interval is automatically calculated based on the number of relay entries.
auto: Automatically calculates the refresh interval. The more the entries, the shorter the refresh interval. The shortest interval is 50 ms.
interval interval: Specifies the refresh interval in the range of 1 to 120 seconds.
# Set the refresh interval to 100 seconds.
[Sysname] dhcp relay client-information refresh interval 100
Use dhcp relay client-information refresh enable to enable the DHCP relay agent to periodically refresh dynamic relay entries.
Use undo dhcp relay client-information refresh enable to disable the DHCP relay agent to periodically refresh dynamic relay entries.
The DHCP relay agent periodically refreshes relay entries.
A DHCP client unicasts a DHCP-RELEASE message to the DHCP server to release its IP address. The DHCP relay agent conveys the message to the DHCP server and does not remove the IP-to-MAC entry of the client.
With this feature, the DHCP relay agent uses a client's IP address and the relay interface's MAC address to periodically send a DHCP-REQUEST message to the DHCP server.
·     If the server returns a DHCP-ACK message or does not return any message within an interval, the DHCP relay agent performs the following operations:
¡     Removes the relay entry.
¡     Sends a DHCP-RELEASE message to the DHCP server to release the IP address.
·     If the server returns a DHCP-NAK message, the relay agent keeps the entry.
With this feature disabled, the DHCP relay agent does not remove relay entries automatically. After a DHCP client releases its IP address, you must use the reset dhcp relay client-information command on the relay agent to remove the corresponding relay entry.
# Disable periodic refresh of relay entries.
[Sysname] undo dhcp relay client-information refresh enable
dhcp relay dhcp-server timeout
Use dhcp relay dhcp-server timeout to set the DHCP server response timeout time for DHCP server switchover.
Use undo dhcp relay dhcp-server timeout to restore the default.
dhcp relay dhcp-server timeout time
The DHCP server response timeout time is 30 seconds.
Interface view
time: Specifies the DHCP server response timeout time in the range of 30 to 65535 seconds.
# Set the DHCP server response timeout time to 60 seconds for DHCP server switchover on GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp relay dhcp-server timeout 60
dhcp relay server-address algorithm
dhcp relay forward reply by-option82
Use dhcp relay forward reply by-option82 to configure the DHCP relay agent to forward DHCP replies based on Option 82.
Use undo dhcp relay forward reply by-option82 to restore the default.
The DHCP relay agent does not forward DHCP replies based on Option 82.
Interface view
This command takes effect only after you execute the dhcp relay information enable and dhcp relay information circuit-id commands.
# Configure the DHCP relay agent to forward DHCP replies based on Option 82.
[Sysname-GigabitEthernet0/0/1] dhcp relay forward reply by-option82
dhcp relay gateway
Use dhcp relay gateway to specify the DHCP relay agent address to be padded to DHCP requests.
Use undo dhcp relay gateway to restore the default.
dhcp relay gateway ip-address
The primary IP address of the interface is padded to DHCP requests as the DHCP relay agent address.
Interface view
ip-address: Specifies the DHCP relay agent address. It must be an IP address of the interface.
The DHCP relay agent uses the specified IP address instead of the primary IP address of the relay interface as the DHCP relay agent address.
# Specify 10.1.1.1 as the DHCP relay agent address to be padded to DHCP requests on GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp relay gateway 10.1.1.1
gateway-list
Use dhcp relay information circuit-id to configure the padding mode and padding format for the Circuit ID sub-option of Option 82.
Use undo dhcp relay information circuit-id to restore the default.
dhcp relay information circuit-id { bas [ sub-interface-vlan ] [ with-vxlan ] | srv6-opcode | string circuit-id | { normal | verbose [ node-identifier { mac | sysname | user-defined node-identifier } ] [ interface ] } [ sub-interface-vlan ] [ format { ascii | hex } ] }
The padding mode is normal and the padding format is hex.
Interface view
bas: Specifies the bas mode that fills in the Circuit ID sub-option with the interface and VLAN information. The device fills the information in the format of interface-type slot/subslot/port vxlan_id.vlan_id.subvlan_id.
sub-interface-vlan: Specifies the VLAN ID of the L2VE subinterface as the content for the Circuit ID sub-option. If you do not specify this keyword, the VLAN ID of the interface on which you configure this command is written to the sub-option. This keyword is available only for L3VE interfaces.
with-vxlan: Specifies the bas mode with VXLAN ID. If you do not specify this keyword, you specify the bas mode without VXLAN ID.
srv6-opcode: Specifies the SRv6 opcode mode that inserts the SRv6 opcode of the relay interface into the Circuit ID sub-option. On receipt of the relayed DHCP request, the server allocates an IP address and network settings according to the padded opcode.
string circuit-id: Specifies the string mode that uses a case-sensitive string of 3 to 63 characters as the content of the Circuit ID sub-option.
normal: Specifies the normal mode, in which the padding content consists of the VLAN ID and port number.
verbose: Specifies the verbose mode. The padding content includes the node identifier, interface information, and VLAN ID. The default node identifier is the MAC address of the access node. The default interface information consists of the Ethernet type (fixed to eth), chassis number, slot number, sub-slot number, and interface number.
node-identifier { mac | sysname | user-defined node-identifier }: Specifies the access node identifier.
·     mac: Uses the MAC address of the access node as the node identifier.
·     sysname: Uses the device name as the node identifier. You can set the device name by using the sysname command in system view. The padding format for the device name is always ASCII regardless of the specified padding format.
If sysname is specified as the node identifier, do not include any spaces when you set the device name. Otherwise, the DHCP relay agent fails to add or replace Option 82.
·     user-defined node-identifier: Uses a case-sensitive string of 1 to 50 characters as the node identifier. The padding format for the specified character string is always ASCII regardless of the specified padding format.
interface: Uses the interface name as the interface information. The padding format for the interface name is always ASCII regardless of the specified padding format.
format: Specifies the padding format for the Circuit ID sub-option.
ascii: Specifies the ASCII padding format.
hex: Specifies the hex padding format.
The Circuit ID sub-option cannot carry information about interface splitting or subinterfaces. For more information about interface splitting and subinterfaces, see Interface Configuration Guide.
The padding format for the string mode, the normal mode, or the verbose mode varies by command configuration. Table 9 shows how the padding format is determined for different modes.
Table 9 Padding format for different modes
Keyword (mode)
If no padding format is set
If the padding format is ascii
If the padding format is hex
string circuit-id
The padding format is ASCII, and is not configurable.
N/A
N/A
normal
Hex.
ASCII.
Hex.
verbose
Hex for the VLAN ID.
ASCII for the node identifier, Ethernet type, chassis number, slot number, sub-slot number, and interface number.
ASCII.
ASCII for the node identifier and Ethernet type.
Hex for the chassis number, slot number, sub-slot number, interface number, and VLAN ID.
# Specify the content mode as verbose, node identifier as the device name, and the padding format as ASCII for the Circuit ID sub-option.
[Sysname-GigabitEthernet0/0/1] dhcp relay information enable
[Sysname-GigabitEthernet0/0/1] dhcp relay information strategy replace
[Sysname-GigabitEthernet0/0/1] dhcp relay information circuit-id verbose node-identifier sysname format ascii
display dhcp relay information
Use dhcp relay information enable to enable the DHCP relay agent to support Option 82.
Use undo dhcp relay information enable to disable Option 82 support.
The DHCP relay agent does not support Option 82.
Interface view
This command enables the DHCP relay agent to add Option 82 to DHCP requests that do not contain Option 82 before forwarding the requests to the DHCP server. The content of Option 82 is determined by the dhcp relay information circuit-id and dhcp relay information remote-id commands. If the DHCP requests contain Option 82, the relay agent handles the requests according to the strategy configured with the dhcp relay information strategy command.
If this feature is disabled, the relay agent forwards requests that contain or do not contain Option 82 to the DHCP server.
# Enable Option 82 support on the relay agent.
Use dhcp relay information remote-id to configure the padding mode and padding format for the Remote ID sub-option of Option 82.
Use undo dhcp relay information remote-id to restore the default.
Interface view
normal: Specifies the normal mode in which the padding content is the MAC address of the receiving interface.
format: Specifies the padding format for the Remote ID sub-option. The default padding format is hex.
string remote-id: Specifies the string mode that uses a case-sensitive string of 1 to 63 characters as the content of the Remote ID sub-option.
sysname: Specifies the sysname mode that uses the device name as the content of the Remote ID sub-option. You can set the device name by using the sysname command.
The padding format for the specified character string (string) or the device name (sysname) is always ASCII. The padding format for the normal mode is determined by the command.
# Specify the padding content for the Remote ID sub-option of Option 82 as device001.
[Sysname-GigabitEthernet0/0/1] dhcp relay information remote-id string device001
Use dhcp relay information strategy to configure the strategy for the DHCP relay agent to handle messages containing Option 82.
Use undo dhcp relay information strategy to restore the default handling strategy.
The handling strategy for messages that contain Option 82 is replace.
Interface view
drop: Drops DHCP messages that contain Option 82 messages.
keep: Keeps the original Option 82 intact and forwards the DHCP messages.
replace: Replaces the original Option 82 with the configured Option 82 before forwarding the DHCP messages.
This command takes effect only on DHCP requests that contain Option 82.
For DHCP requests that do not contain Option 82, the DHCP relay agent always adds Option 82 to the requests before forwarding the requests to the DHCP server.
If the handling strategy is replace, configure a padding mode and padding format for Option 82. If the handling strategy is keep or drop, you do not need to configure any padding mode or padding format. The settings do not take effect even if you configure them.
# Specify the handling strategy for Option 82 as keep.
[Sysname-GigabitEthernet0/0/1] dhcp relay information strategy keep
dhcp relay mac-forward enable
Use dhcp relay mac-forward enable to enable MAC address table lookup for DHCP replies that do not have forwarding information on the relay agent.
Use undo dhcp relay mac-forward enable to restore the default.
dhcp relay mac-forward enable [ broadcast ]
The DHCP relay agent discards a DHCP reply if the agent does not have the forwarding information for the reply.
broadcast: Broadcasts DHCP replies out of the interface in the matching MAC address entry. If you do not specify this keyword, the DHCP relay agent unicasts DHCP replies.
# Enable MAC address table lookup for DHCP replies that do not have forwarding information on the relay agent.
[Sysname] dhcp relay mac-forward enable
dhcp relay master-server switch-delay
Use dhcp relay master-server switch-delay to enable the switchback to the master DHCP server and set the switchback delay time.
Use undo dhcp relay master-server switch-delay to restore the default.
dhcp relay master-server switch-delay delay-time
The DHCP relay agent does not switch back to the master DHCP server.
Interface view
delay-time: Specifies the delay time in the range of 1 to 65535 minutes.
# Configure the DHCP relay agent to switch back to the master DHCP server 3 minutes after it switches to a backup DHCP server on GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp relay master-server switch-delay 3
dhcp relay release ip
Use dhcp relay release ip to release a client IP address.
ip-address: Specifies the IP address to be released.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the specified IP address belongs. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command releases the IP address on the public network.
After you execute this command, the relay agent sends a DHCP-RELEASE packet to the DHCP server and removes the relay entry of the IP address. Upon receiving the packet, the server removes binding information about the specified IP address to release the IP address.
# Release IP address 1.1.1.1.
[Sysname] dhcp relay release ip 1.1.1.1
dhcp relay request-from-tunnel discard
Use dhcp relay request-from-tunnel discard to configure the DHCP relay agent to discard the DHCP requests received from SRv6 tunnels.
Use undo dhcp relay request-from-tunnel discard to restore the default.
The DHCP relay agent forwards the DHCP requests received from SRv6 tunnels.
SRv6 VSI interface view
On an SRv6 network, the DHCP relay agent feature can be configured on the VSI interface of a PE.
When the DHCP relay agent receives a DHCP request from an access unit mapped to the VSI interface, the relay agent forwards this request to the DHCP servers and broadcasts this request to other PEs. If those PEs also function as DHCP relay agents, each will forward the DHCP request to the DHCP servers they are connecting to. To prevent a DHCP server from receiving the same DHCP request from different PEs, you can configure this command on the VSI interface of each PE that is not directly connecting to DHCP clients.
# Configure the DHCP relay agent to discard the DHCP requests received from SRv6 tunnels.
[Sysname] interface vsi-interface 1
[Sysname-Vsi-interface1] dhcp relay request-from-tunnel discard
Use dhcp relay server-address to specify DHCP servers on the DHCP relay agent.
Use undo dhcp relay server-address to remove DHCP servers.
dhcp relay server-address ip-address
undo dhcp relay server-address [ ip-address ]
No DHCP server is specified on the DHCP relay agent.
Interface view
ip-address: Specifies the IP address of a DHCP server. The DHCP relay agent forwards DHCP packets received from DHCP clients to this DHCP server.
The specified IP address of the DHCP server must not reside on the same subnet as the IP address of the DHCP relay agent interface. Otherwise, the DHCP clients might fail to obtain IP addresses.
You can specify a maximum of eight DHCP servers on an interface. The DHCP relay agent forwards the packets from the clients to all the specified DHCP servers.
If you do not specify an IP address, the undo dhcp relay server-address command removes all DHCP servers on the interface.
# Specify DHCP server address 1.1.1.1 on GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp relay server-address 1.1.1.1
dhcp select relay
display dhcp relay interface
Use dhcp relay server-address algorithm to specify the DHCP server selecting algorithm.
Use undo dhcp relay server-address algorithm to restore the default.
dhcp relay server-address algorithm { master-backup | polling }
The polling algorithm is used. The DHCP relay agent forwards DHCP requests to all DHCP servers at the same time.
Interface view
master-backup: Forwards DHCP requests to the master DHCP server first. If the master server is not available or does not have assignable IP addresses, the relay agent forwards DHCP requests to backup DHCP servers in the order they are specified.
polling: Forwards DHCP requests to all DHCP servers at the same time.
# Specify master-backup as the DHCP server selecting algorithm on GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp relay server-address algorithm master-backup
remote-server algorithm
dhcp relay source-address
Use dhcp relay source-address to specify the source IP address for DHCP requests.
Use undo dhcp relay source-address to restore the default.
dhcp relay source-address { ip-address [ option { 60 [ option-text ] | code } ] | gateway | interface interface-type interface-number | relay-interface }
undo dhcp relay source-address { ip-address [ option { 60 [ option-text ] | code } ] | gateway | interface | relay-interface }
The relay agent chooses the default source IP address for relayed requests depending on whether its server-side interface and the DHCP server belong to the same VPN instance:
·     If they belong to the same VPN instance, the relay agent uses the IP address of the output interface for relayed requests as the source IP address.
·     If they belong to different VPN instances, the relay agent uses the lowest IP address that is in the same VPN instance as the DHCP server as the source address.
Interface view
ip-address: Specifies the source IP address for DHCP requests. This IP address will also be filled in the giaddr field.
option { 60 [ option-text ] | code }: Changes the source IP address and the giaddr field of a DHCP request if the DHCP request carries the specified option. If you do not specify any option, this command changes the source IP address and the giaddr field of all DHCP requests that the interface receives.
·     60 [ option-text ]: Identifies packets by the content of Option 60. The content is a case-sensitive string of 1 to 128 characters.
·     code: Specifies an option code in the range of 1 to 59, and 61 to 254.
gateway: Uses the IP address in the giaddr field as the source IP address of the DHCP requests. If the giaddr field is empty, the relay agent follows the default rule to specify the source IP address for DHCP requests.
interface interface-type interface-number: Uses the IP address of an interface as the source IP address. The interface-type interface-number arguments specify an interface by its type and number. If the specified interface has no IP addresses, the relay agent follows the default rule to specify the source IP address for DHCP requests.
relay-interface: Uses the primary IP address of the relay interface as the source IP address. If this interface does not have an IP address, the relay agent follows the default rule to specify the source IP address for DHCP requests.
If you specify the ip-address argument, the relay agent changes not only the source IP address but also the giaddr field of a DHCP request. The DHCP server assigns the client an IP address on the same subnet as the specified IP address in the giaddr field. As a result, the DHCP client might not be on the same subnet as the DHCP relay interface (the gateway). To avoid this problem, you must configure Option 82 on the relay agent before specifying the ip-address argument. This configuration enables the DHCP relay agent to insert the primary IP address of the relay interface in Option 82. Based on this option, the DHCP server assigns an IP address on the same subnet as the IP address of the relay interface. The DHCP relay agent looks up the MAC address table for the output interface to forward the DHCP reply.
If you do not specify any options, the undo dhcp relay source-address command removes all configured source IP addresses for DHCP requests on the interface.
The source IP addresses specified by the following commands overwrite each other, whichever is configured the last:
·     The dhcp relay source-address ip-address command without any DHCP options specified.
·     The dhcp relay source-address interface command.
·     The dhcp relay source-address gateway command.
·     The dhcp relay source-address relay-interface command.
The dhcp relay source-address ip-address option { 60 [ option-text ] | code } and dhcp relay source-address { ip-address | gateway | interface | relay-interface } commands do not overwrite each other.
If multiple sources IP addresses are specified on an interface, their match order is as follows:
1.     Source IP addresses specified with DHCP options are sorted in descending order of option values. A big DHCP option value has a priority. To match Option 60, the source IP address with the option-text argument takes precedence over the source IP address without the option-text argument.
2.     Source IP addresses specified by the dhcp relay source-address ip-address commands without any DHCP options specified.
# Specify 1.1.1.1 as the source IP address for DHCP requests on GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp relay source-address 1.1.1.1
dhcp-server timeout
Use dhcp-server timeout to set the DHCP server response timeout time for DHCP server switchover.
Use undo dhcp-server timeout to restore the default.
# Set the DHCP server response timeout time to 60 seconds for DHCP server switchover in DHCP address pool 0.
[Sysname-dhcp-pool-0] dhcp-server timeout 60
dhcp smart-relay enable
Use dhcp smart-relay enable to enable the DHCP smart relay feature.
Use undo dhcp smart-relay enable to disable the DHCP smart relay feature.
The DHCP smart relay feature is disabled.
The smart relay feature allows the relay agent to use secondary IP addresses as the gateway address when the DHCP server does not reply the DHCP-OFFER message. The relay agent initially encapsulates its primary IP address to the giaddr field before forwarding a request to the DHCP server. If no DHCP-OFFER is returned after two retries, the relay agent switches to secondary IP addresses.
Without this feature, the relay agent always uses the primary IP address as the gateway address.
# Enable the DHCP smart relay feature.
[Sysname] dhcp smart-relay enable
dhcp select
gateway-list
display dhcp relay check mac-address
Use display dhcp relay check mac-address to display MAC address check entries on the relay agent.
# Display MAC address check entries on the DHCP relay agent.
<Sysname> display dhcp relay check mac-address
Source-MAC        Interface                 Aging-time
23f3-1122-adf1    GE0/0/1                   10
23f3-1122-2230    GE0/0/2                   30
Table 10 Command output
Source MAC
Source MAC address of the attacker.
Interface where the attack comes from.
Aging-time
Aging time of the MAC address check entry, in seconds.
display dhcp relay client-information
Use display dhcp relay client-information to display relay entries on the relay agent.
interface interface-type interface-number: Displays relay entries on the specified interface. If you do not specify an interface, this command displays relay entries on all interfaces.
ip ip-address: Displays the relay entry for the specified IP address. If you do not specify an IP address, this command displays relay entries for all IP addresses.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the specified IP address belongs. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command displays the relay entry for the specified IP address on the public network.
The DHCP relay agent records relay entries only after you configure the dhcp relay client-information record command.
# Display all relay entries on the relay agent.
<Sysname> display dhcp relay client-information
Total number of client-information items: 2
Total number of dynamic items: 1
Total number of temporary items: 1
IP address       MAC address      Type        Interface            VPN name
10.1.1.1         00e0-0000-0001   Dynamic     GE0/0/1              N/A
10.1.1.5         00e0-0000-0000   Temporary   GE0/0/1              N/A
# Display relay entries for the specified IP address.
<Sysname> display dhcp relay client-information ip 10.1.1.1
Total number of client-information items: 1
Total number of temporary items: 0
IP address       : 10.1.1.5
MAC address      : 00e0-0000-0000
Type             : Dynamic
Port index       : N/A
Interface        : Vlan2
VPN name         : N/A
Server address   : 12.1.1.2
Access type      : CommonV4
Outer VLAN       : N/A
Inner VLAN       : N/A
PPP index        : 0
Table 11 Command output
Total number of relay entries.
Total number of dynamic relay entries.
Total number of temporary relay entries.
IP address
IP address of the DHCP client.
MAC address
MAC address of the DHCP client.
Relay entry type:
·     Dynamic—The relay agent creates a dynamic relay entry upon receiving an ACK response from the DHCP server.
·     Temporary—The relay agent creates a temporary relay entry upon receiving a REQUEST packet from a DHCP client.
Layer 3 interface connected to the DHCP client. N/A is displayed for relay entries without interface information.
VPN name
Name of the VPN instance to which the DHCP client belongs. If the DHCP client does not belong to any VPN, this field displays N/A.
Port index
Layer 2 port that receives the DHCP request. If the request is not received through a Layer 2 port, this field displays N/A.
Server address
IP address of the DHCP server.
Access type
Access type of the DHCP client:
·     Commonv4—Portal or DHCP.
·     IPoEv4—IPoE.
·     PPPv4—PPP.
Outer VLAN
Outer VLAN tag contained in the DHCP request. If the request does not contain an outer VLAN tag, this field displays N/A.
Inner VLAN
Inner VLAN tag contained in the DHCP request. If the request does not contain an inner VLAN tag, this field displays N/A.
PPP index
PPP session index. If no PPP session index exists, this field displays N/A.
Use display dhcp relay information to display Option 82 configuration information for the DHCP relay agent.
interface interface-type interface-number: Displays Option 82 configuration information for the specified interface. If you do not specify an interface, this command displays Option 82 configuration information about all interfaces.
# Display Option 82 configuration information for all interfaces.
<Sysname> display dhcp relay information
Interface: GigabitEthernet0/0/1
   Status: Enable
   Strategy: Replace
   Circuit ID Pattern: Verbose
   Remote ID Pattern: Sysname
   Circuit ID format: Undefined
   Remote ID format: ASCII
   Node identifier: aabbcc
Interface: GigabitEthernet0/0/2
   Status: Enable
   Strategy: Replace
   Circuit ID Pattern: User Defined
   Remote ID Pattern: User Defined
   Circuit ID format: ASCII
   User defined:
   Circuit ID: vlan100
   Remote ID: device001
Table 12 Command output
Interface name.
Status
Option 82 states:
·     Enable—DHCP relay agent support for Option 82 is enabled.
·     Disable—DHCP relay agent support for Option 82 is disabled.
Strategy
Handling strategy for request messages containing Option 82, Drop, Keep, or Replace.
Circuit ID Pattern
Padding content mode of the Circuit ID sub-option, Verbose, Normal, SRv6-opcode, or User Defined.
Remote ID Pattern
Padding content mode of the Remote ID sub-option, Sysname, Normal, or User Defined.
Circuit ID format-type
Padding format of the Circuit ID sub-option, ASCII, Hex, or Undefined.
Remote ID format-type
Padding format of the Remote ID sub-option, ASCII, Hex, or Undefined.
Node identifier
Access node identifier.
User defined
Content of the user-defined sub-options.
Circuit ID
User-defined content of the Circuit ID sub-option.
Remote ID
User-defined content of the Remote ID sub-option.
display dhcp relay server-address
Use display dhcp relay server-address to display DHCP server addresses configured on an interface.
interface interface-type interface-number: Displays DHCP server addresses on the specified interface. If you do not specify an interface, this command displays DHCP server addresses on all interfaces.
# Display DHCP server addresses on all interfaces.
<Sysname> display dhcp relay server-address
Interface name                 Server IP address
GE0/0/1                        2.2.2.2
# Display DHCP server addresses on the GigabitEthernet 0/0/1.
<Sysname> display dhcp relay server-address interface gigabitethernet 0/0/1
Active server address: 2.2.2.2
GE0/0/1                        2.2.2.2
Table 13 Command output
Active DHCP server address. The displayed value depends on the DHCP server selecting algorithm configuration.
·     If the polling algorithm is used, this field displays all. The DHCP relay agent forwards DHCP requests to all DHCP servers.
·     If the master-backup algorithm is used, this field displays the IP address of the active DHCP server. The DHCP relay agent forwards DHCP requests to the master DHCP server first.
Interface name
Interface name.
Server IP address
DHCP server IP address.
display dhcp relay statistics
Use display dhcp relay statistics to display DHCP packet statistics on the DHCP relay agent.
interface interface-type interface-number: Displays DHCP packet statistics on the specified interface. If you do not specify an interface, this command displays all DHCP packet statistics on the DHCP relay agent.
# Display all DHCP packet statistics on the DHCP relay agent.
<Sysname> display dhcp relay statistics
DHCP packets dropped:                  0
DHCP packets received from clients:    0
   DHCPDISCOVER:                       0
   DHCPREQUEST:                        0
   DHCPINFORM:                         0
   DHCPRELEASE:                        0
   DHCPDECLINE:                        0
   BOOTPREQUEST:                       0
DHCP packets received from servers:    0
   DHCPOFFER:                          0
   DHCPACK:                            0
   DHCPNAK:                            0
   BOOTPREPLY:                         0
DHCP packets relayed to servers:       0
   DHCPDISCOVER:                       0
   DHCPREQUEST:                        0
   DHCPINFORM:                         0
   DHCPRELEASE:                        0
   DHCPDECLINE:                        0
   BOOTPREQUEST:                       0
DHCP packets relayed to clients:       0
   DHCPOFFER:                          0
   DHCPACK:                            0
   DHCPNAK:                            0
   BOOTPREPLY:                         0
DHCP packets sent to servers:          0
   DHCPDISCOVER:                       0
   DHCPREQUEST:                        0
   DHCPINFORM:                         0
   DHCPRELEASE:                        0
   DHCPDECLINE:                        0
   BOOTPREQUEST:                       0
DHCP packets sent to clients:          0
   DHCPOFFER:                          0
   DHCPACK:                            0
   DHCPNAK:                            0
   BOOTPREPLY:                         0
reset dhcp relay statistics
gateway-list
Use gateway-list to specify gateway addresses for DHCP clients in a DHCP address pool.
Use undo gateway-list to remove gateway addresses from a DHCP address pool.
gateway-list ip-address&<1-64> [ export-route ]
undo gateway-list [ ip-address&<1-64> ] [ export-route ]
No gateway address is specified in a DHCP address pool.
DHCP address pool view
ip-address&<1-64>: Specifies a space-separated list of up to 64 addresses.
export-route: Binds the gateways to the device's MAC address in the address management module. The ARP module will use the entries to reply to ARP requests from the DHCP clients. If you do not specify this keyword, the gateways will not be bound to the device's MAC address.
DHCP clients of the same access type can be classified into different types by their locations. In this case, the relay interface typically has no IP address configured. You can use the gateway-list command to specify gateway addresses for clients matching the same DHCP address pool and bind the gateway addresses to the device's MAC address.
Upon receiving a DHCP DISCOVER or REQUEST from a client that matches a DHCP address pool, the relay agent processes the packet as follows:
1.     Fills the giaddr field of the packet with a specified gateway address.
2.     Forwards the packet to all DHCP servers in the matching DHCP address pool.
The DHCP servers select a DHCP address pool according to the gateway address.
# Specify gateway address 10.1.1.1 in DHCP address pool 0.
[Sysname] dhcp server ip-pool 0
[Sysname-dhcp-pool-0] gateway-list 10.1.1.1
Use master-server switch-delay to enable the switchback to the master DHCP server and set the switchback delay time.
Use undo master-server switch-delay to restore the default.
# Configure the DHCP relay agent to switch back to the master DHCP server 3 minutes after it switches to a backup DHCP server in DHCP address pool 0.
[Sysname-dhcp-pool-0] master-server switch-delay 3
remote-server
Use remote-server to specify DHCP servers for a DHCP address pool.
Use undo remote-server to remove DHCP servers from a DHCP address pool.
remote-server ip-address&<1-8>
undo remote-server [ ip-address&<1-8> ]
No DHCP server is specified for the DHCP address pool.
ip-address&<1-8>: Specifies a space-separated list of up to eight DHCP server addresses.
If you do not specify a DHCP server address, the undo remote-server command removes all DHCP servers in the DHCP address pool.
# Specify DHCP server 10.1.1.1 for DHCP address pool 0.
[Sysname-dhcp-pool-0] remote-server 10.1.1.1
Use remote-server algorithm to specify the DHCP server selecting algorithm.
Use undo remote-server algorithm to restore the default.
remote-server algorithm { master-backup | polling }
# Specify master-backup as the DHCP server selecting algorithm in DHCP address pool 0.
[Sysname-dhcp-pool-0] remote-server algorithm master-backup
dhcp-server timeout
remote-server
Use reset dhcp relay client-information to clear relay entries on the DHCP relay agent.
interface interface-type interface-number: Clears relay entries on the specified interface. If you do not specify an interface, this command clears relay entries on all interfaces.
ip ip-address: Clears the relay entry for the specified IP address. If you do not specify an IP address, this command clears relay entries for all IP addresses.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the specified IP address belongs. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If you do not specify a VPN instance, this command clears the relay entry for the specified IP address on the public network.
# Clear all relay entries on the DHCP relay agent.
<Sysname> reset dhcp relay client-information
Use reset dhcp relay statistics to clear relay agent statistics.
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command clears all DHCP relay agent statistics.
# Clear all DHCP relay agent statistics.
<Sysname> reset dhcp relay statistics
DHCP client commands
dhcp client dad enable
Use dhcp client dad enable to enable duplicate address detection.
Use undo dhcp client dad enable to disable duplicate address detection.
Duplicate address detection is enabled.
DHCP client detects IP address conflict through ARP packets. An attacker can act as the IP address owner to send an ARP reply. This makes the client unable to use the IP address assigned by the server. As a best practice, disable duplicate address detection when ARP attacks exist on the network.
# Disable the duplicate address.
[Sysname] undo dhcp client dad enable
dhcp client dscp
Use dhcp client dscp to set the DSCP value for DHCP packets sent by the DHCP client.
Use undo dhcp client dscp to restore the default.
dhcp client dscp dscp-value
The DSCP value is 56 in DHCP packets sent by the DHCP client.
dscp-value: Sets the DSCP value for DHCP packets, in the range of 0 to 63.
The DSCP value of a packet specifies the priority level of the packet and affects the transmission priority of the packet. A bigger DSCP value represents a higher priority.
# Set the DSCP value to 30 for DHCP packets sent by the DHCP client.
[Sysname] dhcp client dscp 30
dhcp client identifier
Use dhcp client identifier to configure a DHCP client ID for an interface.
Use undo dhcp client identifier to restore the default.
An interface generates the DHCP client ID based on its MAC address. If the interface has no MAC address, it uses the MAC address of the first Ethernet interface to generate its client ID.
Interface view
ascii ascii-string: Specifies a case-sensitive ASCII string of 1 to 63 characters as the client ID.
hex hex-string: Specifies a hexadecimal number of 4 to 64 characters as the client ID.
mac interface-type interface-number: Uses the MAC address of the specified interface as a DHCP client ID. The interface-type interface-number argument specifies an interface by its type and number.
A DHCP client ID is added to the DHCP option 61. A DHCP server can specify IP addresses for clients based on the DHCP client ID. You can specify a DHCP client ID by performing one of the following operations:
·     Naming an ASCII string or hexadecimal number as the client ID.
·     Using the MAC address of an interface to generate a client ID.
Whichever method you use, make sure the IDs for different DHCP clients are unique.
# Use the MAC address of GigabitEthernet 0/0/2 as the DHCP client ID for GigabitEthernet 0/0/1.
[Sysname-GigabitEthernet0/0/1] dhcp client identifier mac gigabitethernet 0/0/2
display dhcp client
display dhcp client
Use display dhcp client to display DHCP client information.
verbose: Displays detailed DHCP client information. If you do not specify this keyword, the command displays brief DHCP client information.
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays DHCP client information on all interfaces.
# Display brief DHCP client information on all interfaces.
<Sysname> display dhcp client
GigabitEthernet0/0/1 DHCP client information:
 Current state: BOUND
 Allocated IP: 40.1.1.20 255.255.255.0
 Allocated lease: 259200 seconds, T1: 129600 seconds, T2: 226800 seconds
 DHCP server: 40.1.1.2
# Display detailed DHCP client information on all interfaces.
<Sysname> display dhcp client verbose
 Transaction ID: 0x1c09322d
 Default router: 40.1.1.2
Classless static routes:
   Destination: 1.1.0.1, Mask: 255.0.0.0, NextHop: 192.168.40.16
   Destination: 10.198.122.63, Mask: 255.255.255.255, NextHop: 192.168.40.16
 DNS servers: 44.1.1.11 44.1.1.12
 Domain name: ddd.com
 Boot servers: 200.200.200.200  1.1.1.1
 ACS parameter:
   URL: http://192.168.1.1:7547/acs
   Username: bims
   Password: ******
 Client ID value: 000c.29d3.8659-GE0/0/1
                            6433-2e38-3635-392d-
                            4574-6830-2f30-2f32
 T1 will timeout in 1 day 11 hours 58 minutes 52 seconds.
Table 14 Command output
Information about the interface that acts as the DHCP client.
Current state
Current state of the DHCP client:
·     HALT—The client stops applying for an IP address.
·     INIT—The initialization state.
·     SELECTING—The client has sent out a DHCP-DISCOVER message in search for a DHCP server and is waiting for the response from DHCP servers.
·     REQUESTING—The client has sent out a DHCP-REQUEST message requesting for an IP address and is waiting for the response from DHCP servers.
·     BOUND—The client has received the DHCP-ACK message from a DHCP server and obtained an IP address successfully.
·     RENEWING—The T1 timer expires.
·     REBOUNDING—The T2 timer expires.
Allocated IP
IP address allocated by the DHCP server.
Allocated lease
Allocated lease time.
T1
1/2 lease time (in seconds) of the DHCP client IP address.
T2
7/8 lease time (in seconds) of the DHCP client IP address.
Lease from….to….
Start and end time of the lease.
DHCP server
DHCP server IP address that assigned the IP address.
Transaction ID
Transaction ID, a random number chosen by the client to identify an IP address allocation.
Default router
Gateway address assigned to the client.
Classless static routes assigned to the client.
Static routes
Classful static routes assigned to the client.
DNS servers
DNS server address assigned to the client.
Domain name
Domain name suffix assigned to the client.
Boot servers
PXE server addresses (up to 16 addresses) specified for the DHCP client, which are obtained through Option 43.
ACS parameter
Parameters about the ACS.
URL
URL of the ACS.
Username
Username for logging in to the ACS.
Password
Password for logging in to the ACS. If a password is configured, this field displays ******. If no password is configured, this field is not displayed.
Client ID type
DHCP client ID type:
·     If an ASCII string is used as the client ID value, the type value is 00.
·     If the MAC address of a specific interface is used as the client ID value, the type value is 01.
·     If a hexadecimal number is used as the client ID value, the type value is the first two characters in the string.
Client ID value
Value of the DHCP client ID.
DHCP client ID with the type field, a hexadecimal number.
How long the T1 (1/2 lease time) timer will timeout.
ip address dhcp-alloc
Use ip address dhcp-alloc to configure an interface to use DHCP for IP address acquisition.
Use undo ip address dhcp-alloc to cancel an interface from using DHCP.
An interface does not use DHCP for IP address acquisition.
Interface view
When you execute the undo ip address dhcp-alloc command, the interface sends a DHCP-RELEASE message to release the IP address obtained through DHCP. If the interface is down, the message cannot be sent out. This situation can occur when a subinterface obtained an IP address through DHCP, and the shutdown command is executed on its primary interface. The subinterface will fail to send a DHCP-RELEASE message.
# Configure GigabitEthernet 0/0/1 to use DHCP for IP address acquisition.
[Sysname-GigabitEthernet0/0/1] ip address dhcp-alloc
BOOTP client commands
display bootp client
Use display bootp client to display information about a BOOTP client.
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays BOOTP client information on all interfaces.
# Display BOOTP client information on GigabitEthernet 0/0/1.
<Sysname> display bootp client interface gigabitethernet 0/0/1
GigabitEthernet0/0/1 BOOTP client information:
Allocated IP: 169.254.0.2 255.255.0.0
Transaction ID: 0x3d8a7431
MAC Address: 00e0-fc0a-c3ef
Table 15 Command output
Information about the interface that acts as a BOOTP client.
Allocated IP
BOOTP client's IP address allocated by the BOOTP server.
Transaction ID
Value of the XID field in a BOOTP message. The BOOTP client chooses a random number for the XID field when sending a BOOTP request to the BOOTP server. It is used to match a response message from the BOOTP server. If the values of the XID field are different in the BOOTP response and request, the BOOTP client drops the BOOTP response.
Mac Address
MAC address of a BOOTP client.
ip address bootp-alloc
Use ip address bootp-alloc to configure an interface to use BOOTP for IP address acquisition.
Use undo ip address bootp-alloc to cancel an interface from using BOOTP.
An interface does not use BOOTP for IP address acquisition.
Interface view
# Configure GigabitEthernet 0/0/1 to use BOOTP for IP address acquisition.
[Sysname-GigabitEthernet0/0/1] ip address bootp-alloc