08-Network Management and Monitoring Command Reference
HomeSupportWirelessWX3000E Series Wireless SwitchesReference GuidesCommand ReferencesH3C WX3000E Series Wireless Switches Switching Engine Command References(R3507P26)-6W10208-Network Management and Monitoring Command Reference
04-PoE Commands
04-PoE Commands 162.21 KB
PoE configuration commands
The term "switch" or "device" in this chapter refers to the switching engine on a WX3000E wireless switch.
The WX3000E series comprises WX3024E and WX3010E wireless switches.
The port numbers in this chapter are for illustration only.
apply poe-profile
apply poe-profile { index index | name profile-name }
undo apply poe-profile { index index | name profile-name }
View
PoE interface view
Default level
2: System level
index index: Index number of the PoE configuration file, which ranges from 1 to 100.
name profile-name: Name of the PoE configuration file, which is a string of 1 to 15 characters.
Use the apply poe-profile command to apply the PoE configuration file to the current PoE interface.
Use the undo apply poe-profile command to remove the application of the PoE configuration file to the current PoE interface.
The index number, instead of the name, of the PoE configuration file is displayed when you execute the display this command.
Related commands: display poe-profile and apply poe-profile interface.
# Apply the PoE configuration file named forIPphone to PoE interface GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] apply poe-profile name forIPphone
[Sysname-GigabitEthernet1/0/1] display this
 apply poe-profile index 1
return
apply poe-profile { index index | name profile-name } interface interface-range
undo apply poe-profile { index index | name profile-name } interface interface-range
View
Default level
2: System level
interface-range: Range of Ethernet interface numbers, indicating multiple Ethernet interfaces. The expression is interface-range = interface-type interface-number [ to interface-type interface-number ], where interface-type interface-number represents the interface type and interface number. The start interface number should be smaller than the end interface number. Ethernet interface numbers can be in any range. If any interface in the specified range does not support PoE, it is ignored when the PoE configuration file is applied.
Use the apply poe-profile interface command to apply the PoE configuration file to one or more PoE interfaces.
Use the undo apply poe-profile interface command to remove the application of the PoE configuration file to the specified PoE interface(s).
Related commands: display poe-profile interface and apply poe-profile.
[Sysname] apply poe-profile name forIPphone interface gigabitethernet 1/0/1
# Apply the PoE configuration file with index number 1 to PoE interfaces GigabitEthernet 1/0/2 through GigabitEthernet 1/0/8.
[Sysname] apply poe-profile index 1 interface gigabitethernet 1/0/2 to gigabitethernet 1/0/8
display poe device
display poe device [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
|: Filters command output by specifying a regular expression. For more information about regular expressions, see the Fundamentals Configuration Guide.
begin: Displays the first line that matches the specified regular expression and all lines that follow.
exclude: Displays all lines that do not match the specified regular expression.
include: Displays all lines that match the specified regular expression.
regular-expression: Specifies a regular expression, which is a case sensitive string of 1 to 256 characters.
Use the display poe device command to display information about power sourcing equipments (PSEs).
# Display the PSE information. (The output varies with devices.)
<Sysname> display poe device
 PSE ID  SlotNo SubSNo PortNum  MaxPower(W)  State  Model
 4        1       0       24        170            on      LSW124POED
Table 1 Output description
PSE ID
ID of the PSE. This field takes a value of 1
SlotNo
Slot number of the PSE. This field takes a value of 1
SubSNo
Sub-slot number of the PSE. This field takes a value of 0
PortNum
Number of PoE interfaces on the PSE
MaxPower(W)
Maximum power of the PSE (W)
PSE state:
·       on: The PSE is supplying power.
·       off: The PSE stops supplying power.
·       faulty: The PSE fails.
Model
PSE model
display poe interface
display poe interface [ interface-type interface-number ] [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
Use the display poe interface command to display the power information of the specified interface.
If no interface is specified, the power information of all PoE interfaces is displayed.
# Display the power state of GigabitEthernet 1/0/1.
<Sysname> display poe interface gigabitethernet 1/0/1
 Port Power Enabled                   : disabled
 Port Power Priority                  : low
 Port Operating Status                : power-deny
 Port IEEE Class                       : 0
 Port Detection Status                : disabled
 Port Power Mode                       : signal
 Port Current Power                  : 0   mW
 Port Average Power                   : 0   mW
 Port Peak Power                       : 0   mW
 Port Max Power                        : 25000    mW
 Port Current                          : 0   mA
 Port Voltage                          : 0.0   V
 Port PD Description                  : IP Phone For Room 101
Table 2 Output description
Port Power Enabled
PoE state—enabled/disabled
Port Power Priority
Power priority of the PoE interface:
·       critical (highest)
·       high
·       low
Operating state of a PoE interface:
·       offPoE is disabled.
·       on: Power is supplied for a PoE interface normally.
·       power-lack—the guaranteed remaining power of the PSE is not high enough to supply power for a critical PoE interface.
·       power-deny—the PSE refuses to supply power. The power required by the powered device (PD) is higher than the configured power.
·       power-itself—the external equipment is supplying power for itself.
·       power-limit—the PSE is supplying a limited power. The power required by the PD is higher than the configured power and the PSE still supplies the configured power.
Port IEEE class
PD power class—0, 1, 2, 3, 4, and -
- indicates not supported.
Power detection state of a PoE interface:
·       disabled—the PoE function is disabled.
·       searching: The PoE interface is searching for the PD.
·       delivering-power—the PoE interface is supplying power for the PD.
·       fault—there is a fault defined in 802.3af.
·       test: The PoE interface is under test.
·       other-fault—there is a fault other than defined in 802.3af.
·       pd-disconnect—the PD is disconnected.
Port Power Mode
Power mode of a PoE interface is signal
Port Current Power
Current power of a PoE interface, including PD consumption power and transmission loss
Port Average Power
Average power of a PoE interface
Port Peak Power
Peak power of a PoE interface
Port Max Power
Maximum power of a PoE interface
Port Current
Current of a PoE interface
Port Voltage
Voltage of a PoE interface
Port PD Description
Description of the PD connected to the PoE interface, which is used to identify the type and location of the PD.
# Display the state of all PoE interfaces.
Interface    Status   Priority CurPower Operating  IEEE   Detection
                                (W)      Status     Class  Status
 GE1/0/1      disabled low      0.0      power-deny 0      disabled
 GE1/0/2      disabled low      0.0      power-deny 0      disabled
 GE1/0/3      disabled low      0.0      power-deny 0      disabled
 GE1/0/4      disabled low      0.0      power-deny 0      disabled
 GE1/0/5      disabled low      0.0      power-deny 0      disabled
 GE1/0/6      disabled low      0.0      power-deny 0      disabled
 GE1/0/7      disabled low      0.0      power-deny 0      disabled
 GE1/0/8      disabled low      0.0      power-deny 0      disabled
 GE1/0/9      disabled low      0.0      power-deny 0      disabled
 GE1/0/10     disabled low      0.0      power-deny 0      disabled
 GE1/0/11     disabled low      0.0      power-deny 0      disabled
 GE1/0/12     disabled low      0.0      power-deny 0      disabled
 GE1/0/13     disabled low      0.0      power-deny 0      disabled
 GE1/0/14     disabled low      0.0      power-deny 0      disabled
 GE1/0/15     disabled low      0.0      power-deny 0      disabled
 GE1/0/16     disabled low      0.0      power-deny 0      disabled
 GE1/0/17     disabled low      0.0      power-deny 0      disabled
 GE1/0/18     disabled low      0.0      power-deny 0      disabled
 GE1/0/19     disabled low      0.0      power-deny 0      disabled
 GE1/0/20     disabled low      0.0      power-deny 0      disabled
 GE1/0/21     disabled low      0.0      power-deny 0      disabled
 GE1/0/22     disabled low      0.0      power-deny 0      disabled
 GE1/0/23     disabled low      0.0      power-deny 0      disabled
 GE1/0/24     disabled low      0.0      power-deny 0      disabled
   ---  0 port(s) on,    0.0 (W) consumed,   170.0 (W) remaining ---
Table 3 Output description
Shortened form of a PoE interface
Enable
Priority
Power priority of a PoE interface:
·       high
·       low
CurPower
Operating Status
·       off—PoE is disabled.
·       on—power is supplied for a PoE interface normally.
IEEE class
PD power class defined by IEEE
Detection Status
·       searching—the PoE interface is searching for the PD.
·       test—the PoE interface is under test.
·       There is a fault other than defined in 802.3af.
port(s) on
Number of PoE interfaces that are supplying power
consumed
Power consumed by the current PoE interface
Remaining
Total remaining power of the system
display poe interface power
display poe interface power [ interface-type interface-number ] [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
Use the display poe interface power command to display the power information of a PoE interface(s).
# Display the power information of GigabitEthernet 1/0/1.
<Sysname> display poe interface power gigabitethernet 1/0/1
Interface   CurPower  PeakPower   MaxPower  PD Description
             (W)       (W)         (W)
 GE1/0/1     0.0       0.0         30.0        Acess Point on Room 509 for Peter
# Display the power information of all PoE interfaces.
             (W)       (W)         (W)
 GE1/0/2     0.0       0.0         30.0
 GE1/0/3     0.0       0.0         30.0
 GE1/0/4     0.0       0.0         30.0
 GE1/0/5     0.0       0.0         30.0
 GE1/0/6     0.0       0.0         30.0
 GE1/0/7     0.0       0.0         30.0
 GE1/0/8     0.0       0.0         30.0
 GE1/0/9     0.0       0.0         30.0
 GE1/0/10    0.0       0.0         30.0
 GE1/0/11    0.0       0.0         30.0
 GE1/0/12    0.0       0.0         30.0
 GE1/0/13    0.0       0.0         30.0
 GE1/0/14    0.0       0.0         30.0
 GE1/0/15    0.0       0.0         30.0
 GE1/0/16    0.0       0.0         30.0
 GE1/0/17    0.0       0.0         30.0
 GE1/0/18    0.0       0.0         30.0
 GE1/0/19    0.0       0.0         30.0
 GE1/0/20    0.0       0.0         30.0
 GE1/0/21    0.0       0.0         30.0
 GE1/0/22    0.0       0.0         30.0
 GE1/0/23    0.0       0.0         30.0
 GE1/0/24    0.0       0.0         30.0
Table 4 Output description
CurPower
PeakPower
MaxPower
PD Description
Description of the PD connected with a PoE interface
port(s) on
consumed
Power currently consumed by all PoE interfaces
Remaining
display poe pse
display poe pse [ pse-id ] [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
pse-id: PSE ID. To view the mapping between PSE ID and slot, use the display poe device command. If you do not specify this parameter, the information of all PSEs on the device is displayed.
Use the display poe pse command to display the information of PSE(s).
# Display the information of the PSE 1
<Sysname> display poe pse 1
PSE ID                           : 1
 PSE Slot No                      : 1
 PSE SubSlot No                   : 0
 PSE Model                        : EWPX124POEPA
 PSE Power Enabled                : enabled
 PSE Power Priority               : -
 PSE Current Power                : 0        W
 PSE Average Power                : 0        W
 PSE Peak Power                   : 0        W
 PSE Max Power                    : 740      W
 PSE Remaining Guaranteed         : 740      W
 PSE CPLD Version                 : -
 PSE Software Version             : 0
 PSE Hardware Version             : 0
 PSE Legacy Detection             : disabled
 PSE Utilization-threshold        : 80
Table 5 Output description
PSE ID
ID of the PSE
PSE Slot No
PSE SubSlot No
Subslot number of the PSE
PSE Model
Model of the PSE module
PSE Power Enabled
PoE is enabled for the PSE
PSE Power Preempted
PSE power preempted state:
no—the power of the PSE is not preempted.
yes—the power of the PSE is preempted so that it cannot supply power, although PoE is enabled for the PSE
PSE Power Priority
Power priority of the PSE
PSE Current Power
Current power of the PSE
PSE Average Power
Average power of the PSE
PSE Peak Power
Peak power of the PSE
PSE Max Power
Guaranteed remaining power of the PSE = Guaranteed maximum power of the PSE– the sum of the maximum power of the critical PoE interfaces of the PSE
PSE CPLD Version
PSE CPLD version
PSE software version number
PSE hardware version number
Nonstandard PD detection by the PSE: enabled or disabled
PSE power alarm threshold
display poe pse interface
display poe pse pse-id interface [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
pse pse-id: Specifies a PSE ID. To view the mapping between PSE ID and slot, use the display poe device command.
Use the display poe pse interface command to display the state of all PoE interfaces connected to the specified PSE.
# Display the state of all PoE interfaces connected to PSE 7.
<Sysname> display poe pse 7 interface
Table 6 Output description
Enable
PoE enabled/disabled state. For the value, see Table 2.
Priority
Priority of a PoE interface. For the value, see Table 2.
CurPower
Operating
Operating state of a PoE interface. For the value, see Table 2.
IEEE
PD power class
Detection
Power detection state of a PoE interface. For the value, see Table 2.
port(s) on
consumed
Power consumed by PoE interfaces on the PSE
Remaining
Remaining power on the PSE
display poe pse interface power
display poe pse pse-id interface power [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
Use the display poe pse interface power command to display the power information of PoE interfaces connected with the PSE.
# Display the power information of PoE interfaces connected with PSE 7.
<Sysname> display poe pse 7 interface power
             (W)       (W)         (W)
Table 7 Output description
CurPower
PeakPower
MaxPower
PD Description
Description of the PD connected with a PoE interface.
port(s) on
consumed
Remaining
display poe-profile
display poe-profile [ index index | name profile-name ] [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
Use the display poe-profile command to display the information of the PoE configuration file.
If no argument is specified, all information of the configurations and applications of existing PoE configuration files is displayed.
# Display the information of all PoE configuration files.
<Sysname> display poe-profile
 Poe-profile     Index   ApplyNum  Interface   Configuration
 forIPphone      1        6          GE1/0/5        poe enable
                                       GE1/0/6         poe priority critical
                                       GE1/0/7
                                       GE1/0/8
                                       GE1/0/9
                                       GE1/0/10
 forAP            2        2          GE1/0/11       poe enable
                                       GE1/0/12       poe max-power 14000
 ---  2 poe-profile(s) created, 8 port(s) applied  ---
# Display the information of the PoE configuration file with index number 1.
<Sysname> display poe-profile index 1
                                       GE1/0/7
                                       GE1/0/8
                                       GE1/0/9
                                       GE1/0/10
 ---  6 port(s) applied  ---
# Display the information of PoE configuration file forIPphone.
<Sysname> display poe-profile name forIPphone
                                        GE1/0/7
                                        GE1/0/8
                                        GE1/0/9
                                        GE1/0/10
Table 8 Output description
Poe-profile
Index
ApplyNum
Number of PoE interfaces to which a PoE configuration file is applied
Shortened form of the PoE interface to which the PoE configuration is applied
Configuration
Configurations of the PoE configuration file
Number of PoE configuration files
port(s) applied
Sum of the number of PoE interfaces to which all PoE configuration files are respectively applied
display poe-profile interface interface-type interface-number [ | { begin | exclude | include } regular-expression ]
View
Default level
1: Monitor level
Use the display poe-profile interface command to display all information of the configurations and applications of the PoE configuration file that currently takes effect on the specified PoE interface.
# Display all information of the configurations and applications of the current PoE configuration file applied to GigabitEthernet 1/0/1.
<Sysname> display poe-profile interface gigabitethernet 1/0/1
 Poe-profile     Index   ApplyNum  Interface   Current Configuration
 forIPphone      1        6          GE1/0/1      poe enable
Not all the configurations of a PoE configuration file can be applied successfully, so only the configurations that currently take effect on the interface are displayed. For the descriptions for other fields, see Table 8.
poe enable
poe enable
undo poe enable
View
PoE interface view, PoE-profile file view
Default level
2: System level
None
Use the poe enable command to enable PoE on a PoE interface.
Use the undo poe enable command to disable PoE on a PoE interface.
By default, PoE is disabled on a PoE interface.
CAUTION
CAUTION:
·       If a PoE configuration file is already applied to a PoE interface, remove the application of the file to the PoE interface before configuring the interface in PoE-profile view.
·       If a PoE configuration file is applied to a PoE interface, remove the application of the file to the PoE interface before configuring the interface in PoE interface view.
# Enable PoE on a PoE interface.
[Sysname-GigabitEthernet1/0/1] poe enable
# Enable PoE on a PoE interface through a PoE configuration file.
[Sysname] poe-profile abc
[Sysname-poe-profile-abc-1] poe enable
[Sysname-poe-profile-abc-1] quit
[Sysname-GigabitEthernet1/0/1] apply poe-profile name abc
poe legacy enable
poe legacy enable pse pse-id
undo poe legacy enable pse pse-id
View
Default level
2: System level
Use the poe legacy enable command to enable the PSE to detect nonstandard PDs.
Use the undo poe legacy enable command to disable the PSE from detecting nonstandard PDs.
By default, the PSE is disabled from detecting nonstandard PDs.
# Enable PSE 7 to detect nonstandard PDs.
[Sysname] poe legacy enable pse 7
poe max-power
poe max-power max-power
undo poe max-power
View
Default level
2: System level
max-power: Maximum power in milliwatts allocated to a PoE interface. The value ranges from 1000 to 25000.
Use the poe max-power command to configure the maximum power for a PoE interface.
Use the undo poe max-power command to restore the default.
By default, the maximum power of the PoE interface is 25000 milliwatts.
# Set the maximum power of GigabitEthernet 1/0/1 to 12000 milliwatts.
[Sysname-GigabitEthernet1/0/1] poe max-power 12000
# Set the maximum power of GigabitEthernet 1/0/1 to 12000 milliwatts through a PoE configuration file.
[Sysname-poe-profile-abc-1] poe max-power 12000
poe mode
poe mode signal
undo poe mode
View
Default level
2: System level
signal: Specifies the PoE mode as signal (power over signal cables), which means to use the pairs (1, 2, 3, 6) for transmitting data in category 3/5 twisted pair cable to supply DC power.
Use the poe mode command to configure a PoE mode.
Use the undo poe mode command to restore the default.
By default, the PoE mode is signal (power over signal cables).
# Set the PoE mode to signal (power over signal cables).
[Sysname-GigabitEthernet1/0/1] poe mode signal
# Set the PoE mode to signal (power over signal cables) through a PoE configuration file.
[Sysname-poe-profile-abc-1] poe mode signal
poe pd-description
poe pd-description text
undo poe pd-description
View
PoE interface view
Default level
2: System level
text: Description of the PD connected to a PoE interface, which is a string of 1 to 80 characters.
Use the poe pd-description command to configure a description for the PD connected to a PoE interface.
Use the undo poe pd-description command to restore the default.
By default, no description is available for the PD connected to a PoE interface.
# Configure the description for the PD connected to GigabitEthernet 1/0/1 as IP Phone for Room 101.
[Sysname-GigabitEthernet1/0/1] poe pd-description IP Phone For Room 101
poe priority
poe priority { critical | high | low }
undo poe priority
View
Default level
2: System level
critical: Sets the power priority of a PoE interface to critical. The PoE interface whose power priority level is critical works in guaranteed mode. In other words, power is first supplied to the PD connected to this critical PoE interface.
high: Sets the power priority of a PoE interface to high.
low: Sets the power priority of a PoE interface to low.
Use the poe priority command to configure a power priority level for a PoE interface.
Use the undo poe priority command to restore the default.
By default, the power priority of a PoE interface is low.
When the PoE power is insufficient, power is first supplied to PoE interfaces with a higher priority level.
If two PoE interfaces have the same priority level, the PoE interface with a smaller ID has the higher priority level.
# Set the power priority of GigabitEthernet 1/0/1 to critical.
[Sysname-GigabitEthernet1/0/1] poe priority critical
# Set the power priority of GigabitEthernet 1/0/1 to critical through a PoE configuration file.
[Sysname-poe-profile-abc-1] poe priority critical
poe update
poe update { full | refresh } filename [ pse pse-id ]
View
Default level
2: System level
full: Specifies to upgrade the PSE processing software in full mode when the software is unavailable.
refresh: Specifies to upgrade the PSE processing software in refresh mode when the software is available.
filename: Name of the upgrade file, which is a string of 1 to 64 characters. This file must be under the root directory of the file system of the device. The extension of the upgrade file is *.s19.
Use the poe update command to upgrade the PSE processing software online.
CAUTION
CAUTION:
·       The full mode is used only in the case that anomalies occur when you use the refresh mode to upgrade the PSE processing software. Do not use the full mode in other circumstances.
·       You can use the full mode to upgrade the PSE processing software to restore the PSE firmware when the PSE processing software is unavailable (it means that none of the PoE commands are executed successfully).
·       If you upgrade the PSE firmware on a backup control board, the upgrade file must be on the main control board, and only the main control board can control the upgrade of the PSE firmware on the backup control board.
# Upgrade the processing software of PSE 7 in service
[Sysname] poe update refresh 0400_001.S19 pse 7
poe utilization-threshold
poe utilization-threshold utilization-threshold-value pse pse-id
undo poe utilization-threshold pse pse-id
View
Default level
2: System level
utilization-threshold-value: Power alarm threshold in percentage, which ranges from 1 to 99.
Use the poe utilization-threshold command to configure a power alarm threshold for the PSE.
Use the undo poe utilization-threshold command to restore the default power alarm threshold of the PSE.
By default, the power alarm threshold for the PSE is 80%.
The system sends a trap message when the power utilization exceeds the alarm threshold. If the power utilization always keeps above the alarm threshold, the system does not send any trap message. Instead, when the percentage of the power utilization drops below the alarm threshold, the system sends a Trap message again.
# Set the power alarm threshold of PSE 7 to 90%
[Sysname] poe utilization-threshold 90 pse 7
poe-profile
poe-profile profile-name [ index ]
undo poe-profile { index index | name profile-name }
View
Default level
2: System level
profile-name: Name of a PoE configuration file, which is a string of 1 to 15 characters. A PoE configuration file name begins with a letter (a through z or A through Z) and must not contain reserved keywords such as undo, all, name, interface, user, poe, disable, max-power, mode, priority and enable.
index: Index number of a PoE configuration file, which ranges from 1 to 100.
Use the poe-profile profile-name command to create a PoE configuration file and enter PoE-profile view.
Use the undo poe-profile command to delete the specified PoE configuration file.
If no index is specified, the system automatically assigns an index to the PoE configuration file, starting from 1.
If a PoE configuration file is already applied to a PoE interface, you cannot delete it. To delete the file, execute the undo apply poe-profile command to remove the application of the PoE configuration file to the PoE interface.
# Create a PoE configuration file, name it abc, and specify the index number as 3.
[Sysname] poe-profile abc 3