12-Network Management and Monitoring Configuration Guide
HomeSupportSwitchesS9850-G SeriesTechnical DocumentsConfigure & DeployConfiguration GuidesH3C S6850-G&S6805-G&S9850-G Switch Series Configuration Guides-R8336Pxx-6W10012-Network Management and Monitoring Configuration Guide
05-PTP configuration
05-PTP configuration 845.74 KB
Configuring PTP·· 1
About PTP· 1
Basic concepts· 1
Protocols and standards· 4
PTP time synchronization mechanisms· 5
Time synchronization basics· 5
Grandmaster clock selection and master-member/subordinate relationship establishment 5
Optimal domain selection· 7
Frequency synchronization mechanism·· 8
Phase synchronization mechanism·· 9
PTP support for IPv6 networks· 10
Association between PTP and Track· 11
Restrictions and guidelines: PTP configuration· 11
PTP tasks at a glance· 11
Configuring PTP (IEEE 1588 version 2) 11
Configuring PTP (IEEE 802.1AS) 13
Configuring PTP (SMPTE ST 2059-2) 13
Configuring PTP (AES67-2015) 14
Specifying PTP for obtaining the time· 15
Enabling PTP message sending by hardware· 15
Creating a PTP instance· 16
Specifying a PTP profile· 16
Configuring clock nodes· 17
Specifying a clock node type· 17
Configuring an OC to operate only as a member clock· 17
Specifying a PTP domain· 18
Configuring the clock source whitelist 18
Enabling PTP globally· 19
Enabling PTP on a port 19
Configuring PTP ports· 20
Configuring the role of a PTP port 20
Configuring the mode for carrying timestamps· 20
Specifying a delay measurement mechanism for a BC or an OC· 21
Configuring one of the ports on a TC+OC clock as an OC-type port 22
Enabling unicast negotiation on PTP ports· 22
Configuring PTP message transmission and receipt 23
Setting the interval for sending announce messages and the timeout multiplier for receiving announce messages  23
Setting the interval for sending Pdelay_Req messages· 24
Setting the interval for sending Sync messages· 24
Setting the minimum interval for sending Delay_Req messages· 25
Setting the interval for sending Delay-Resp messages· 26
Configuring parameters for PTP messages· 26
Specifying the UDP transport protocol for PTP messages· 26
Configuring a source IP address for multicast PTP messages transmitted over UDP· 27
Configuring a destination IP address for unicast PTP messages transmitted over UDP· 27
Configuring the MAC address for non-Pdelay messages· 28
Setting a DSCP value for PTP messages transmitted over UDP· 28
Specifying a VLAN tag for PTP messages· 29
Disabling PTP path tracing· 29
Adjusting and correcting clock synchronization· 30
Setting the delay correction value· 30
Calculating the TAI based on the UTC time· 30
Configuring the PTP offset threshold and PTP synchronization suppressions· 32
Configuring a priority for a clock· 33
Configuring PTP logging· 34
Enabling SNMP notification for the PTP module· 35
About this task· 35
Procedure· 35
Display and maintenance commands for PTP· 35
PTP configuration examples· 36
Example: Configuring PTP (IEEE 1588 version 2, IEEE 802.3/Ethernet transport, multicast transmission) 36
Example: Configuring PTP (IEEE 1588 version 2, UDP transport, multicast transmission) 39
Example: Configuring multiple PTP instances (IEEE 1588 version 2, multicast transmission) 42
Example: Configuring PTP (IEEE 802.1AS, IEEE 802.3/Ethernet transport, multicast transmission) 50
Example: Configuring PTP (SMPTE ST 2059-2, UDP transport, multicast transmission) 53
Example: Configuring PTP (AES67-2015, UDP transport, multicast transmission) 56
Configuring PTP
About PTP
Precision Time Protocol (PTP) provides time synchronization among devices with submicrosecond accuracy. It provides also precise frequency synchronization.
Basic concepts
PTP profile
IEEE 1588 is the basic PTP protocol. It defines the high-precision clock synchronization principle and the message interaction and processing specifications on the network. It was initially used for industrial automation and is now mainly used on bridged local area networks. 1588 has two versions: 1588v1 and 1588v2. 1588v1 can provide time synchronization only with sub-millisecond accuracy, and 1588v2 can provide time synchronization accuracy to the sub-microsecond level and can achieve both phase and frequency synchronization. 1588v2 is more widely used than 1588v1.
Based on 1588, PTP protocols including IEEE 802.1AS, ITU-T G.8275.1, and ITU-T G.8275.2 were developed to adapt to different application scenarios. This document focuses on the implementation mechanism and application scenarios of 1588v2.
·     IEEE 1588 version 2—1588v2 defines high-accuracy clock synchronization mechanisms. It can be customized, enhanced, or tailored as needed. 1588v2 is the latest version.
·     IEEE 802.1AS—802.1AS is introduced based on IEEE 1588. It specifies a profile for use of IEEE 1588-2008 for time synchronization over a virtual bridged local area network (as defined by IEEE 802.1Q). 802.1AS supports only point-to-point full-duplex Ethernet, IEEE 802.11, and IEEE 802.3 EPON links.
·     SMPTE ST 2059-2—ST2059-2 is introduced based on IEEE 1588. It specifies a profile specifically for time synchronization of audio or video equipment in a professional broadcast environment. It includes a self-contained description of parameters, their default values, and permitted ranges.
·     AES67-2015—AES67-2015 is introduced based on IEEE 1588. It specifies a profile specifically for time synchronization of professional equipment for broadcast, music production, and film and television post-production. It includes a self-contained description of parameters, their default values, and permitted ranges.
PTP domain
A PTP domain refers to a network or part of a network that is enabled with PTP. A PTP domain has only one reference clock called "grandmaster clock (GM)." All devices in the domain synchronize to the clock.
PTP instance
If the device belongs to multiple PTP domains, you must configure and associate a PTP instance with each PTP domain. You can configure PTP settings such as PTP profile and clock node type on a PTP instance. The settings take effect only on the PTP domain associated with the PTP instance. PTP instances are isolated from each other, allowing different PTP timing systems to run on a network without affecting each other.
Optimal PTP domain
Each PTP instance has a reference clock and clock information. For a device that has multiple PTP instances running simultaneously, you must select an optimal PTP instance and use the clock source traced by this PTP instance to synchronize the system time of the device. The domain with which the optimal PTP associates is the optimal domain.
Clock node and PTP port
A node in a PTP domain is a clock node. A port enabled with PTP is a PTP port. PTP defines the following types of basic clock nodes:
·     Ordinary Clock (OC)—A PTP clock with a single PTP port in a PTP domain for time synchronization. It synchronizes time from its upstream clock node through the port. If an OC operates as the clock source, it sends synchronization time through a single PTP port to its downstream clock nodes.
·     Boundary Clock (BC)—A clock with more than one PTP port in a PTP domain for time synchronization. A BC uses one of the ports to synchronize time from its upstream clock node. It uses the other ports to synchronize time to the relevant upstream clock nodes. If a BC operates as the clock source, such as BC 1 in Figure 1, it synchronizes time through multiple PTP ports to its downstream clock nodes.
·     Transparent Clock (TC)—A TC does not keep time consistency with other clock nodes. A TC has multiple PTP ports. It forwards PTP messages among these ports and performs delay corrections for the messages, instead of performing time synchronization. TCs include the following types:
¡     End-to-End Transparent Clock (E2ETC)—Forwards all PTP packets in the network and supports calculation of the delay on the entire link.
¡     Peer-to-Peer Transparent Clock (P2PTC)—Forwards only Sync, Follow_Up, and Announce messages, terminates other PTP messages, and supports calculation of the delay on the entire link.
IMPORTANT
IMPORTANT:
When multiple PTP domains are configured on the device, the synchronization performance might fluctuate or decrease, and synchronization failure might occur because of limitation of hardware resources. OC and BC clock nodes do much more work than TCs. As a best practice, configure the device operating in multiple domains as an OC or BC clock node in a maximum of one PTP instance, to decrease calculations, minimize mutual influences between the domains, and optimize the synchronization performance.
Figure 1 shows the positions of these types of clock nodes in a PTP domain.
Figure 1 Clock nodes in a PTP domain
In addition to these basic types of clock nodes, PTP introduces hybrid clock nodes. For example, a TC+OC has multiple PTP ports in a PTP domain. One port is the OC type, and the others are the TC type.
A TC+OC forwards PTP messages through TC-type ports and performs delay corrections. In addition, it synchronizes time through its OC-type port. TC+OCs include these types: E2ETC+OC and P2PTC+OC.
Master-member/subordinate relationship
The master-member/subordinate relationship is automatically determined based on the Best Master Clock (BMC) algorithm. You can also manually specify a role for the clock nodes.
The master-member/subordinate relationship is defined as follows:
·     Master/Member node—A master node sends a synchronization message, and a member node receives the synchronization message.
·     Master/Member clock—The clock on a master node is a master clock (parent clock). The clock on a member node is a member clock.
·     Master/Subordinate port—A master port sends a synchronization message, and a subordinate port receives the synchronization message. The master and subordinate ports can be on a BC or an OC.
·     Grant-port/request-port—The IEEE 1588 version 2 PTP profile supports unicast negotiation. To configure unicast negotiation, you can specify PTP ports as request-ports or grant-ports. A grant-port grants and provides PTP service. A request-port requests and receives PTP service. Typically, a grant-port is in master state. A request-port is in slave state when selected as the port for time synchronization and in listening state when not selected.
A port that neither receives nor sends synchronization messages is a passive port.
Clock source type
A clock node supports the following clock sources:
·     Local clock source—38.88 MHz clock signals generated by a crystal oscillator inside the clock monitoring module.
·     External clock source—Clock signals generated by an external clock device. The signals are received and sent by a 1PPS/ToD port on the device. It is also called a ToD clock source.
A clock node uses the local clock source, which is the 38.88 MHz clock signals generated by a crystal oscillator inside the clock monitoring module.
Grandmaster clock
As shown in Figure 2, the grandmaster clock (GM) is the ultimate source of time for clock synchronization in a PTP domain. It is elected automatically by the clock nodes in the PTP domain. The clock nodes exchange PTP messages and elect the GM by comparing the clock priority, time class, and time accuracy carried in the PTP messages.
You can also specify a GM manually.
Figure 2 Clock nodes in a PTP domain
·     IEEE Std 1588-2008, IEEE Standard for a Precision Clock Synchronization Protocol for Networked Measurement and Control Systems, 2008
·     IEEE 802.1AS, Timing and Synchronization for Time-Sensitive Applications in Bridged Local Area Networks
·     SMPTE ST 2059-2, SMPTE Profile for Use of IEEE-1588 Precision Time Protocol in Professional Broadcast Applications
·     AES67-2015, AES Standard for Audio Applications of Networks-High-Performance Streaming Audio-Over-IP Interoperability, 2015
Time synchronization includes frequency synchronization and phase synchronization. The synchronization requirements vary by networking environments.
Frequency synchronization is also called clock synchronization. If two signals are the same in frequency or if they keep a constant phase difference, the two signals are frequency synchronized. As shown in Figure 3, the two watches have different time, but maintain a constant time difference (6 hours).
Figure 3 Frequency synchronization
Phase synchronization is also called time synchronization. If two signals are the same in frequency and phase (keep phase difference at 0), they are phase synchronized. As shown in Figure 4, the two watches have the same time at all times. Frequency synchronization is the prerequisite of phase synchronization.
Figure 4 Phase synchronization
A GM can be manually specified. It can also be elected through the BMC algorithm as follows:
1.     The clock nodes in a PTP domain exchange announce messages and elect a GM by using the following rules in descending order:
a.     Clock node with higher priority 1.
b.     Clock node with higher time class.
c.     Clock node with higher time accuracy.
d.     Clock node with higher priority 2.
e.     Clock node with a smaller port ID (containing clock number and port number).
The master nodes, member nodes, master ports, and subordinate ports are determined during the process. Then a spanning tree with the GM as the root is generated for the PTP domain.
2.     The master node periodically sends announce messages to the member nodes. If the member nodes do not receive announce messages from the master node, they determine that the master node is invalid, and they start to elect another GM.
Figure 5 BMC comparison rule for GMC selection
Establishing master-member/subordinate relationships
The master-member/subordinate relationships between the clock nodes (except for the TCs) on a PTP network are automatically determined based on the Best Master Clock (BMC) algorithm. You can also manually specify a role for the clock nodes.
The following master-member/subordinate relationships exist:
·     Master/Member node—A master node propagates time synchronization information, and a member node receives time synchronization information.
·     Master/Member clock—The clock on a master node is a master clock. The clock on a member node is a member clock.
·     Master/Subordinate port—A master port propagates time synchronization, and a subordinate port receives time synchronization information. The master and subordinate ports can be on a BC or an OC. A port that neither propagates nor receives timing information is a passive port. Passive ports are used to prevent PTP messages from forming loops.
After the grandmaster clock is elected and master-member/subordinate relationships are established, a loop-free, all connected shortest path tree with the grandmaster clock as the root is established in the PTP domain, as shown in Figure 6. Time is synchronized between the clock nodes in the domain along the path tree.
Figure 6 PTP master-member/subordinate relationships
2.
If only one PTP instance is configured on the device, this PTP instance is the optimal instance of the device. If multiple PTP instances are configured on the device, the optimal PTP instance (domain) is selected by using the following rules in descending order:
1.     Activated instance (with a domain configured).
2.     Instance on which the device is an OC or BC clock node.
3.     Instance on which the clock source has a higher priority 1 value
4.     Instance on which the clock source has a higher time class.
5.     Instance on which the clock source has higher time accuracy.
6.     Instance on which the clock source has a lower offset from the GM.
7.     Instance on which the clock source has a higher priority 2 value.
8.     Instance associated with a PTP domain that has a smaller domain ID.
9.     The PTP instance on which the ptp active force-state command is configured has the lowest priority.
After the grandmaster clock is selected and master-member relationships are established, the master clock sends Sync messages to the member clocks periodically. Assume that the path delay between the master and member clock nodes remains unchanged, if the frequency of the member clock and the master clock are synchronized, the time offset between the master and member clock will be the same at the same intervals, which is T(n+1)–Tn = T(n+1)'–Tn', as shown in Figure 7.
·     If T(n+1)–Tn > T(n+1)'–Tn', the member clock is faster in frequency than the master clock and will reduce its frequency.
·     If T(n+1)–Tn < T(n+1)'–Tn', the member clock is slower in frequency than the master clock and will increase frequency faster.
The member clock uses the formula T(n+1)–Tn / T(n+1)'–Tn' to calculate its frequency ratio with the master clock and adjust its clock frequency accordingly.
PTP frequency synchronization can run in single-step mode or two-step mode. The figure below shows the most commonly used two-step frequency synchronization mode. In single-step mode, Tn' and T(n+1)' timestamps are carried in a Sync message, and no Follow_Up message is sent.
Figure 7 PTP frequency synchronization in two-step mode
PTP frequency synchronization can run in one of the following modes:
·     Single-step mode—Uses Sync and Pdelay_Resp messages to carry timestamps, and does not send follow-up messages (Follow_Up or Pdelay_Resp_Follow_Up). The single-step mode has fewer interactive messages than the two-step mode, and occupies less network bandwidth, but it requires hardware chip support. In single-step mode, a timestamp is assigned before the message is sent. Therefore, the timestamp sent in single-step mode is the estimated message sending time that is not as accurate as the two-step mode.
·     Two-step mode—Uses Follow_Up messages to carry Sync message transmit timestamps and Pdelay_Resp_Follow_Up messages to carry Pdelay_Req message receive and Pdelay_Resp message transmit timestamps. The timestamps sent in two-step mode is the actual sending time of the messages, so the two-step mode is more accurate than the single-step mode and can improve PTP time synchronization accuracy.
After master-member relationships are established between the clock nodes, the master and member clock nodes exchange PTP messages and record the message transmit and receive time. Based on the timestamps, each member clock calculates the path delay and time offset between them and the master clock and adjusts their time accordingly for time synchronization with the master clock.
PTP defines two path delay measurement mechanisms: Request_Response_ and Peer Delay, both of which are based on network symmetry.
Request_Response
The Request_Response mechanism measures the average path delay between the master and member clock nodes by using the PTP messages as shown in Figure 8. A TC between master and member clock nodes does not calculate the path delay. It forwards PTP messages and carries the Sync message residence time on it to the downstream clock node.
This mechanism can be implemented in one of the following two modes:
·     Two-step mode—t1 is carried in the Follow_Up message as shown in Figure 8.
·     Single-step mode—t1 is carried in the Sync message, and no Follow_Up message is sent.
Figure 8 shows the Request_Response mechanism in two-step mode.
1.     The master clock sends a Sync message to the member clock, and records the sending time t1. Upon receiving the message, the member clock records the receiving time t2.
2.     After sending the Sync message, the master clock immediately sends a Follow_Up message that carries time t1.
3.     The member clock sends a Delay_Req message to the master clock, and records the sending time t3. Upon receiving the message, the master clock records the receiving time t4.
4.     The master clock returns a Delay_Resp message that carries time t4.
After this procedure, the member clock obtains all the four timestamps and can make the following calculations:
·     Round-trip delay between the master and member clocks: (t2 t1) + (t4 t3)
·     One-way delay between the master and member clocks: [(t2 – t1) + (t4 – t3)] / 2
·     Offset between the member and master clocks: (t2 – t1) – [(t2 – t1) + (t4 – t3)] / 2 or [(t2 – t1) – (t4 – t3)] / 2
Figure 8 Request_Response mechanism (two-step node)
Peer Delay
The Peer Delay mechanism measures the average path delay between two clock nodes. The two clock nodes (BC, TC, or OC) implementing this mechanism send Pdelay messages to each other, and calculate the one-way link delay between them independently. The message interaction process and delay calculation method are identical on the two nodes. TCs that exist between master and member clock nodes divide the synchronization path into multiple links and participate in delay calculation. The link delays and Sync message residence time on the TCs are carried to downstream nodes.
·     Two-step mode
As shown in Figure 9, Pdelay messages include Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages. t2 is carried in the Pdelay_Resp message, and t3 is carried in the Pdelay_Resp_Follow_Up message.
·     Single-step mode:
Pdelay messages include Pdelay_Req and Pdelay_Resp messages. t3 – t2 is carried in the Pdelay_Resp, and no Pdelay_Resp_Follow_Up message is sent.
Figure 9 uses Clock node B as an example to describe the Peer Delay mechanism.
1.     Clock node B sends a Pdelay_Req message to Clock node A, and records the sending time t1. Upon receiving the message, Clock node A records the receiving time t2.
2.     Clock node A sends a Pdelay_Req message that carries t2 to Clock node B, and records the sending time t3. Upon receiving the message, Clock node B records the receiving time t4.
3.     Clock node A immediately sends a Pdelay_Resp_Follow_Up message carrying t3 to Clock node B after sending the Pdelay_Req message.
After this procedure, Clock node B obtains all the four timestamps and can make the following calculations:
·     Round-trip delay between Clock node A and Clock node B: (t2 – t1) + (t4 – t3)
·     One-way delay between Clock node A and Clock node B: [(t2 – t1) + (t4 – t3)] / 2 = [(t4 – t1) – (t3 – t2)] / 2
·     Time offset between the member clock and the master clock: Sync message receiving time on the member clock Sync message sending time on the master clock – Total one-way delays on all links – Total Sync message residence time on all TCs.
Figure 9 Peer Delay mechanism (two-step mode)
By default, PTP is encapsulated in Layer 2 packets and can be deployed in both IPv4 and IPv6 networks. If the ptp transport-protocol command is configured, PTP packets are transmitted using the UDP protocol. To deploy PTP in IPv6 and use multicast to send PTP packets, use the ptp source ipv6 ipv6-address [ vpn-instance vpn-instance-name ] command to configure a source IPv6 address for PTP. To use unicast to send PTP packets, use the ptp unicast-destination ipv6 ipv6-address command to configure a destination IPv6 address for PTP.
If you associate a track entry with PTP, and then associate the track entry with an EAA policy, automatic monitoring of the PTP clock source and PTP clock state can be achieved. This enables the device to use PTP to synchronize the system clock when PTP is operating correctly, and use NTP to synchronize the system clock when PTP is not operating correctly.
After you configure this feature, the device creates a track entry associated with PTP. The state of the track entry depends on the state of the associated PTP object. The device supports associating Track with the following types of PTP objects:
·     Clock source—Determines the state of the track entry based on the clock source state in the specified instance.
¡     If the PTP clock source already exists in the specified PTP instance (that is, the device has a subordinate port, and the device is not a GM in the network), the track entry state is Positive.
¡     If the PTP clock source is lost in the specified PTP instance (that is, the device is a GM in the network), the track entry state is Negative.
·     PTP time state—Determines the state of the track entry based on the PTP time state.
¡     If the PTP time state is Lock, the track entry state is Positive.
¡     If the PTP time state is Unlock, the track entry state is Negative.
You can use the Boolean AND tracked list to monitor both the PTP clock source state and PTP time state. For more information about PTP, see "Configuring track" in High Availability Configuration Guide.
Before configuring PTP, determine the PTP profile and define the scope of the PTP domain and the role of every clock node.
In a PTP domain that runs the IEEE 1588 version 2 or IEEE 802.1AS PTP profile,, specify the BC or OC clock node type for the devices in the domain as a best practice. A TC clock node is mainly used for forwarding PTP messages. When receiving a PTP message, a TC multicasts the message from all its PTP interfaces except the inbound interface of the PTP message. To deploy a TC in the domain, plan the TC location and number and location of PTP interfaces on the TC manually to prevent PTP forwarding loops.
Do not assign an interface to multiple PTP instances or PTP domains. If you do so, the device will fail in PTP synchronization with the master device.
The device does not support configuring the interface speed to 1000 Mbps to match the peer interface.
1.     Specifying PTP for obtaining the time
2.     (Optional.) Enabling PTP message sending by hardware
3.     (Optional.) Creating a PTP instance
4.     Specifying a PTP profile
Specify the IEEE 1588 version 2 PTP profile.
5.     Configuring clock nodes
¡     Specifying a clock node type
¡     (Optional.) Configuring an OC to operate only as a member clock
6.     Specifying a PTP domain
7.     (Optional.) Configuring the clock source whitelist
8.     Enabling PTP.
For PTP to run on an interface, enable PTP globally and on the interface.
¡     Enabling PTP globally
¡     Enabling PTP on a port
9.     Configuring PTP ports
¡     (Optional.) Configuring the role of a PTP port
¡     Configuring the mode for carrying timestamps
¡     Specifying a delay measurement mechanism for a BC or an OC
¡     Configuring one of the ports on a TC+OC clock as an OC-type port
¡     (Optional.) Enabling unicast negotiation on PTP ports
10.     (Optional.) Configuring PTP message transmission and receipt
¡     Setting the interval for sending announce messages and the timeout multiplier for receiving announce messages
¡     Setting the interval for sending Pdelay_Req messages
¡     Setting the interval for sending Sync messages
¡     Setting the minimum interval for sending Delay_Req messages
¡     Setting the interval for sending Delay-Resp messages
11.     (Optional.) Configuring parameters for PTP messages
¡     Specifying the UDP transport protocol for PTP messages
¡     Configuring a source IP address for multicast PTP messages transmitted over UDP
¡     Configuring a destination IP address for unicast PTP messages transmitted over UDP
¡     Configuring the MAC address for non-Pdelay messages
¡     Setting a DSCP value for PTP messages transmitted over UDP
¡     Specifying a VLAN tag for PTP messages
¡     Disabling PTP path tracing
12.     (Optional.) Adjusting and correcting clock synchronization
¡     Setting the delay correction value
¡     Calculating the TAI based on the UTC time
¡     Configuring the PTP offset threshold and PTP synchronization suppressions
13.     (Optional.) Configuring a priority for a clock
14.     (Optional.) Configuring PTP logging
15.     (Optional.) Enabling SNMP notification for the PTP module
2.     (Optional.) Creating a PTP instance
3.     Specifying a PTP profile
Specify the IEEE 802.1AS PTP profile.
4.     Configuring clock nodes
5.     (Optional.) Specifying a PTP domain
6.     (Optional.) Configuring the clock source whitelist
7.     Enabling PTP.
8.     Configuring PTP ports
9.     (Optional.) Configuring PTP message transmission and receipt
10.     (Optional.) Specifying a VLAN tag for PTP messages
11.     (Optional.) Disabling PTP path tracing
12.     (Optional. ) Adjusting and correcting clock synchronization
Specify the SMPTE ST 2059-2 PTP profile.
7.     Enabling PTP.
10.     (Optional.) Configuring parameters for PTP messages
11.     (Optional.) Adjusting and correcting clock synchronization
12.     (Optional.) Configuring a priority for a clock
13.     (Optional.) Configuring PTP logging
14.     (Optional.) Enabling SNMP notification for the PTP module
Specify the AES67-2015 PTP profile.
7.     Enabling PTP.
2.     Specify PTP for obtaining the time.
clock protocol ptp
By default, the device uses NTP to obtain the system time.
For more information about the clock protocol command, see device management commands in Fundamentals Command Reference.
This feature improves PTP clock synchronization accuracy. It is applicable to scenarios requiring high-frequency PTP Sync message transmission. With this feature enabled, the hardware directly encapsulates and sends Sync messages. This increases transmission frequency while maintaining device performance and clock synchronization accuracy.
You can execute this command only when the PTP profile is IEEE 1588 version 2 and the clock node type is BC or OC.
This feature is not supported when a non-default PTP instance exists in the system.
If you execute the ptp syn-interval command to set a small Sync message sending interval (higher frequency) without this feature enabled, the configuration will fail.
Disabling this feature restores the Sync message sending interval to the default value for all PTP-enabled interfaces on the specified slot.
2.     Enable PTP message sending by hardware.
ptp hardware enable slot slot-number
A PTP instance is uniquely identified by its ID on a device. For easy identification and management, you can also set a name for a PTP instance.
Do not set the same name for different PTP instances.
If you create PTP instances with the same ID but different names, the most recent configuration takes effect.
The default PTP instance with an ID of 0 has been created by default. You cannot delete the default PTP instance. PTP settings configured in system view take effect only on PTP instance 0. To configure settings for a PTP instance other than PTP instance 0, enter PTP instance view.
You cannot create new PTP instances if PTP message sending by hardware is enabled for default PTP instance 0.
2.     Create a PTP instance.
ptp instance ptp-instance-id [ name ptp-instance-name ]
By default, PTP instance numbered 0 and named default-instance exists.
You must specify a PTP profile before configuring PTP settings. Changing the PTP profile restores all settings under the profile to the default.
1.     ‍Enter system view.
2.     (Optional.) Enter PTP instance view.
To configure settings for PTP instance 0, skip this step.
3.     Specify a PTP profile.
ptp profile { 1588v2 | 8021as | aes67-2015 | st2059-2 }
By default, no PTP profile is configured, and PTP is not running on the device.
Before you specify a clock node type, specify a PTP profile.
Changing the clock node type restores all settings to the default except for the PTP profile.
3.     Specify a clock node type for the device.
¡     IEEE 1588v2 PTP profile:
ptp mode { bc | e2etc | e2etc-oc | oc | p2ptc | p2ptc-oc }
¡     IEEE 802.1AS PTP profile:
ptp mode { bc | oc | p2ptc | p2ptc-oc }
¡     AES67-2015 or SMPTE ST 2059-2 PTP profile:
ptp mode { bc | e2etc | oc | p2ptc }
By default, no clock node type is specified.
An OC can operate either as a master clock to send synchronization messages or as a member clock to receive synchronization messages. This task allows you to configure an OC to operate only as a member clock.
If an OC is operating only as a member clock, you can use the ptp force-state command to configure its PTP port as a master port or passive port.
This task is applicable only to OCs.
3.     Configure the OC to operate only as a member clock.
ptp slave-only
By default, an OC operates as a master or member clock.
This command is mutually exclusive with the ptp unicast-negotiate command.
Within a PTP domain, all devices follow the same rules to communicate with each other. Devices in different PTP domains cannot exchange PTP messages.
3.     Specify a PTP domain for the device.
ptp domain value
By default, no PTP domain exists.
Do not configure the same domain on different PTP instances.
Application scenarios
In large network environments, especially when multiple grandmaster (GM) clocks exist, enabling the clock source whitelist can enhance network stability and security. This function restricts devices to synchronize time only from known and trusted clock sources on the whitelist, thereby avoiding malicious clock attacks and network time oscillations.
Operating mechanism
By default, when an interface with PTP enabled receives a PTP clock synchronization signal, it uses the Best Clock Master Algorithm (BCMA) to select a clock source from multiple clock signals. Devices within the same PTP clock synchronization network will use the time of this selected clock source as their reference and maintain time synchronization with it.
When the clock source whitelist is enabled and the whitelist entries are specified, only clock sources on the whitelist will participate in the clock source election and be considered for PTP time synchronization by the device. If the currently synchronized clock source is not on the whitelist, the device stops synchronizing with that clock source. The clock source whitelist configured in PTP instance view is only effective for that PTP instance, and the whitelist configured in system view is only effective for PTP instance 0. Each PTP instance independently elects its clock source based on its whitelist.
Before enabling the clock source whitelist, make sure the whitelist includes all trusted clock sources, including the primary clock source and all backup clock sources.
To configure the default instance with an instance ID of 0, skip this step.
Make sure the PTP domain is different for different instances.
3.     Add a clock source to the clock source whitelist.
ptp whitelist clockid clock-id
By default, the clock source whitelist does not exist.
4.     Enable the clock source whitelist.
ptp whitelist clockid enable
By default, the clock source whitelist is disabled.
For PTP to run on an interface, you must enable PTP globally and on the interface.
2.     Enable PTP globally.
ptp global enable
By default, PTP is enabled globally.
A port enabled with PTP becomes a PTP port.
You can enable PTP on only one port on an OC.
To enable PTP on a Layer 3 Ethernet interface that has been assigned to a VPN instance, you must execute the ptp source command and specify the VPN instance if PTP messages are to be transmitted in multicast mode over UDP.
2.     Enter Layer 2 Ethernet interface view or Layer 3 Ethernet interface view.
3.     (Optional.) Assign the interface to a PTP instance and enter interface PTP instance view.
4.     Enable PTP on the port.
ptp enable
By default, PTP is disabled on a port.
You can configure the master, passive, or slave role for a PTP port.
For an OC that operates in slave-only mode, you can perform this task to change its PTP port role to master or slave.
·     You can configure one subordinate port on the device.
4.     Configure the role of the PTP port.
ptp force-state { master | passive | slave }
By default, the PTP port role is automatically calculated through BMC.
5.     Return to system view.
6.     (Optional.) Enter PTP instance view.
7.     Activate the port role configuration.
By default, the port role configuration is not activated.
Timestamps can be carried in either of the following modes:
·     Single-step mode—The Sync message (in the Request_Response or Peer Delay mechanism) and Pdelay_Resp message (in the Peer Delay mechanism) carry their sending timestamps by themselves.
·     Two-step mode—The Sync message (in the Request_Response or Peer Delay mechanism) and Pdelay_Resp message (in the Peer Delay mechanism) do not carry their sending timestamps by themselves. The subsequent messages carry their sending timestamps.
The IEEE 802.1AS PTP profile supports only the two-step timestamp-carrying mode.
The device supports only the two-step timestamp-carrying mode when the clock node type is E2ETC, P2PTC, E2ETC+OC, or P2PTC+OC.
4.     Configure the mode for carrying timestamps.
ptp clock-step { one-step | two-step }
By default, the two-step mode is used for carrying  timestamps.
PTP defines two transmission delay measurement mechanisms: Request_Response and Peer Delay. For correct communication, ports on the same link must share the same delay measurement mechanism.
Follow these restrictions and guidelines when you configure this task:
·     IEEE 1588 version 2, SMPTE ST 2059-2, or AES67-2015 PTP profile:
¡     You can configure this task only when the PTP clock node type is BC or OC.
¡     You cannot configure this taks when the PTP clock node type is E2ETC, E2ETC+OC, P2PTC, or P2PTC+OC. The E2ETC and E2ETC+OC clock nodes support both the request-response and peer delay measurement mechanisms. The P2PTC clock node supports only the peer delay measurement mechanism.
·     IEEE 802.1AS PTP profile: Supports only the peer delay measurement mechanism and does not support this task.
4.     Specify a delay measurement mechanism for a BC or an OC.
ptp delay-mechanism { e2e | p2p }
The default setting varies by PTP profile:
¡     IEEE 1588 version 2, AES67-2015, or SMPTE ST 2059-2—The request-response delay measurement mechanism applies.
¡     IEEE 802.1ASThe peer delay measurement mechanism applies.
The ptp delay-mechanism p2p command is mutually exclusive with the ptp unicast-negotiate command.
All ports on a TC+OC (E2ETC+OC or P2PTC+OC) are TC-type ports by default. This feature allows you to configure one of the ports on a TC+OC clock as an OC-type port.
This task is applicable only to E2ETC+OCs and P2PTC+OCs.
This task is not available for the SMPTE ST 2059-2 or AES67-2015 PTP profile.
For time synchronization accuracy, the OC-type port on an E2ETC+OC or P2PTC+OC must be specified as the master port.
4.     Configure the port type as OC.
ptp port-mode oc
By default, the port type for all ports on a TC+OC is TC.
On a network where the IEEE 1588 version 2 PTP profile runs, you can use this task to establish master-subordinate relations between PTP ports by specifying the request-ports and grant-ports. A grant-port grants and provides PTP service. A request-port requests and receives PTP service. Typically, a grant-port is in master state. A request-port is in slave state when selected as the port for time synchronization and in listening state when not selected.
A request-port initiates a PTP link connection request to a specific grant-port. Then they negotiate PTP parameters and exchange PTP messages to synchronize the client time to the server. Plan the network in advance and specify the ports on the member (client) clock nodes as request-ports and the ports on the master (server) clock nodes as grant-ports.
Only the IEEE 1588 version 2 profile supports this task.
Follow these restrictions and guidelines to configure unicast negotiation under the IEEE 1588 version 2 PTP profile:
·     The ptp transport-protocol udp command must be configured for unicast negotiation to take effect.
·     The E2ETC, P2PTC, and P2PTC-OC clock nodes do not support unicast negotiation
·     The ptp unicast-negotiate command is mutually exclusive with the ptp slave-only, ptp force-state, and ptp delay-mechanism p2p commands.
2.     Enter Layer 3 Ethernet interface view.
3.     (Optional.) Assign the interface to a PTP instance and enter PTP instance view.
Skip this step for PTP instance 0.
4.     Enable unicast negotiation and specify the port as a grant-port or request port.
ptp unicast-negotiate { grant-port | request-port }
A master node periodically sends announce messages at the specified interval. If a member node does not receive any announce message from the master node after the timeout expires, it determines that the master node is invalid. The timeout = timeout multiplier × interval at which the master node sends announce messages.
The interval at which the master node sends announce messages depends on whether unicast negotiation is enabled.
·     If unicast negotiation is not enabled, the master node uses the value configured by using the ptp announce-interval command on its interface as the interval.
·     If unicast negotiation is enabled, you must configure the interval on the request-port of the client. The request-port uses the configured interval to negotiate with the grant-port on the server for the interval at which the grant-port sends announce messages to the client. If the negotiation succeeds, the grant-port sends announce messages at the configured interval to the client. If the negotiation fails, the grant-port does not send announce messages to the client.
4.     Set the interval for sending announce messages.
ptp announce-interval interval
The default settings vary by PTP profile.
¡     IEEE 1588 version 2 or AES67-2015—The interval argument value is 1 and the interval for sending announce messages is 2 (21) seconds.
¡     IEEE 802.1AS—The interval argument value is 0 and the interval for sending announce messages is 1 (20)second.
¡     SMPTE ST 2059-2—The interval argument value is –2 and the interval for sending announce messages is 1/4 (2-2) seconds.
5.     Set the number of intervals before a timeout occurs.
ptp announce-timeout multiple-value
By default, a timeout occurs when three intervals are reached.
4.     Set the interval for sending Pdelay_Req messages.
ptp pdelay-req-interval interval
By default, the interval argument value is 0 and the interval for sending peer delay request messages is 1 (20) second.
For the SMPTE ST 2059-2 or AES67-2015 PTP profile, set the interval argument to a value in the range of ptp syn-interval interval to ptp syn-interval interval plus 5 as a best practice.
The master node sends Sync messages to the member nodes periodically. The interval at which the master node sends Sync messages to member nodes depends on whether unicast negotiation is enabled.
·     If unicast negotiation is not enabled, use  this task to configure the interval on the master node.
·     If unicast negotiation is enabled, you must configure the interval on the request-port of the client. The request-port uses the configured interval to negotiate with the grant-port on the server for the interval at which the grant-port sends Sync messages to the client. If the negotiation succeeds, the grant-port sends Sync messages at the configured interval to the client. If the negotiation fails, the grant-port does not send Sync messages to the client.
4.     Set the interval for sending Sync messages.
¡     IEEE 1588 version 2—The interval argument value is 0 and the interval for sending Sync messages is 1 (20) second.
¡     IEEE 802.1AS, AES67-2015, or SMPTE ST 2059-2—The interval argument value is –3 and the interval for sending Sync messages is 1/8 (2-3) seconds.
When receiving a Sync or Follow_Up message, an interface can send Delay_Req messages only when the minimum interval is reached. This task allows you to set the minimum interval for sending Delay_Req messages.
This setting is not available for the IEEE 802.1AS PTP profile.
In PTP multicast transport mode, this setting takes effect only when configured on the master clock. The master clock sends the value to a member clock through PTP messages to control the interval for the member clock to send Delay_Req messages. To view the interval, execute the display ptp interface command on the member clock.
In PTP unicast transport mode, this setting takes effect when configured on member clocks. It does not take effect when configured on the master clock.
4.     Set the minimum interval for sending Delay_Req messages.
ptp min-delayreq-interval interval
The interval argument value is 0 and the minimum interval for sending delay request messages is 1 (20) second.
For the SMPTE ST 2059-2 PTP profile, set the interval argument to a value in the range of ptp syn-interval interval to ptp syn-interval interval plus 5 as a best practice.
This task, configured on a unicast negotiation request-port, specifies the interval at which the grant-port sends Delay_resp messages to the request-port. After receiving a Delay_req message from a request port, the grant-port responds by sending a Delay_resp message and starts a timer defined by this command. The grant-port will not send another Delay_resp message until it receives a Delay_req message after the timer expires.
This task is available only for the IEEE 1588 version 2 PTP profile and is configured on unicast negotiation request-ports.
4.     Set the interval for sending Delay_resp messages.
ptp delay-resp-interval interval
By default, the value of the interval argument is 0 and the minimum interval for sending Delay_resp messages is 1 (20) seconds.
PTP messages can be transported over IEEE 802.3/Ethernet or UDP.
The IEEE 802.1AS PTP profile supports only IEEE 802.3/Ethernet transport of PTP messages and does not support this task.
The SMPTE ST 2059-2 or AES67-2015 PTP profile supports only UDP transport of PTP messages and does not support this task.
4.     Specify the UDP transport protocol for PTP messages.
By default, PTP messages are transported over IEEE 802.3/Ethernet.
To transport multicast PTP messages over UDP, you must configure a source IP address for the messages.
If both a source IP address for multicast PTP messages transmitted over UDP and a destination address for unicast PTP messages transmitted over UDP are configured, the system unicasts the messages.
This task is not available for the IEEE 802.1AS PTP profile.
3.     Configure a source IP address for multicast PTP messages transmitted over UDP.
ptp source{ ip-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ]
By default, no source IP address is configured for multicast PTP messages transmitted over UDP.
To transport unicast PTP messages over UDP, you must configure a destination IP address for the messages.
Configure an IP address for the current interface, and make sure the interface and the peer PTP interface can reach each other.
4.     Configure a destination IP address for unicast PTP messages transmitted over UDP.
ptp unicast-destination { ip-address | ipv6 ipv6-address }
By default, no destination IP address is configured for unicast PTP messages transmitted over UDP.
Pdelay messages include Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages. The destination MAC address of Pdelay messages is 0180-C200-000E by default, which cannot be modified. The destination MAC address of non-Pdelay messages is either 0180-C200-000E or 011B-1900-0000.
This feature takes effect only when PTP messages are encapsulated in IEEE 802.3/Ethernet packets.
This task is not available for the IEEE 802.1AS, SMPTE ST 2059-2, or AES67-2015 PTP profile.
4.     Configure the destination MAC address for non-Pdelay messages.
ptp destination-mac mac-address
The default destination MAC address is 011B-1900-0000.
The DSCP value determines the sending precedence of PTP messages transmitted over UDP.
4.     Set a DSCP value for PTP messages transmitted over UDP.
ptp dscp dscp
By default, the DSCP value is 56.
Perform this task to configure the VLAN ID and the 802.1p precedence in the VLAN tag carried by PTP messages.
2.     Enter Layer 2 Ethernet interface view.
4.     Specify a VLAN tag for PTP messages.
ptp vlan vlan-id [ dot1p dot1p-value ]
By default, PTP messages do not have a VLAN tag.
PTP path tracing traces the clock nodes that the clock signals traverse from the GM to the device. The system can obtain complete path tracing information only when all clock nodes on the path are enabled with PTP path tracing. If a device on the path does not support PTP path tracing, disable this feature to prevent PTP intercommunication issues.
2.     Disable PTP path tracing.
ptp path-trace disable
By default, PTP path tracing is enabled.
PTP performs time synchronization based on the assumption that the delays in sending and receiving messages are the same. However, this is not practical. If you know the offset between the delays in sending and receiving messages, you can set the delay correction value for more accurate time synchronization.
4.     Set a delay correction value.
ptp asymmetry-correction { minus | plus } value
The default is 0 nanoseconds. Delay correction is not performed.
UTC and TAI
International Atomic Time (TAI) is a high-precision atomic coordinate time scale. Coordinated Universal Time (UTC) is based on TAI and adjusted by leap seconds for synchronization with astronomical time.
UTC is constantly compared with UT1 (astronomical time, reflecting the earth's rotation). The International Bureau of Weights and Measures (BIPM) will notify to add or subtract one second from the UTC time scale at the last minute on a specific date (typically June 30 or December 31) to ensure that the difference between UTC and UT1 is within one second.
The BIPM publishes the difference between UTC and TAI periodically. Till now, UTC is 37 seconds behind TAI.
Internet devices typically use the UTC time. To provide more accurate time, PTP also uses TAI. If the device acts as a subordinate clock node, it uses the UTC time and TAI time of the clock reference. The device locally has the following clock sources: one is UTC time (time generated by the local oscillator on the device MPU), and the other is TAI time (also known as PTP time, which is produced by the clock module/PTP chip). If the device acts as the clock reference, it will calculate the TAI time based on the UTC time, and synchronize the UTC and TAI time to the subordinate clocks. This task is used to calculate the TAI time based on the UTC time.
Adjustment of the deviation between UTC and TAI
TAI = Current UTC + cumulative offset + leap second that might occur in the future. To get the correct TAI time from the UTC time,
·     Set the accurate UTC time on the device.
·     Use the ptp utc offset command to set the cumulative offset of UTC relative to TAI as published by BIPM. This command takes effect immediately.
·     If the BIPM notifies to add or subtract one second from the UTC time scale on a specific data after you use the ptp utc offset command to configure the cumulative offset of TAI relative to UTC, use the ptp utc { leap59-date | leap61-date } date command to change the UTC time. The TAI time will be changed accordingly.
UTC and TAI synchronization
When the device is used as the GM clock in a network, and services that rely on PTP time synchronization are deployed in the network (such as iFIT measurement and deterministic networking technology.), jumps in PTP time can affect service operation. Configuring the synchronization of TAI time using UTC time can reduce the jumps in PTP time and thereby minimize the impact of PTP time jumps on services.
When the device is used as the GM clock in the network, the device will perform the following by default:
1.     The device uses its own UTC time as the reference clock source for the entire network.
2.     After the network administrator enables the PTP function in the interface view, the device synchronizes UTC time to the clock module/PTP chip.
3.     Once the clock module/PTP chip synchronizes with the UTC time of this device, the device uses the timing frequency of the clock module/PTP chip for timing and uses TAI time to synchronize PTP time to downstream devices.
4.     The device automatically synchronizes UTC time to the clock module/PTP chip that has the PTP function enabled every 6 hours.
5.     If the network administrator modifies the UTC time (for example, by configuring the clock data-time, ptp utc offset, or ptp utc { leap59-date | leap61-date } commands), the device immediately and automatically synchronizes the updated UTC time to the clock module/PTP chip. This ensures that the UTC time of devices in the network is consistent with the UTC time of this device.
Because TAI time and UTC time are synchronized and then counted separately according to their respective frequencies, extremely subtle deviations might exist between TAI time and UTC time. Synchronizing TAI time with UTC time every 6 hours can cause jumps in TAI time, which in turn causes jumps across the entire network time, further affecting the operation of services that depend on PTP time synchronization.
To avoid this issue, you can synchronize TAI time to UTC time. The device will synchronize TAI time to UTC time every 6 hours, thus avoiding time jumps that affect the entire network.
This setting takes effect only when it is configured on the master clock node and the local clock of the master clock node is the GM.
Configure this feature on both the master and member nodes for the new master clock to provide accurate TAI time after a master/member node switchover.
3.     Set the cumulative offset of UTC relative to TAI.
ptp utc offset utc-offset
The default is 0 seconds.
4.     Add or subtract one second from the UTC time scale at the last minute on the specified date.
By default, no second is added or subtracted from the UTC time.
5.     Enable the device to synchronize the UTC time to the TAI time when the device acts as the GM clock.
ptp refclock-master sync-utc
By default, the device synchronizes the UTC time to the TAI time when it acts as the GM clock.
This function is designed to prevent clock source jumps. Through this mechanism, the device can effectively handle clock jumps, ensure time synchronization recovery after the clock source stabilizes, and avoid time synchronization errors caused by sudden clock changes.
Operating mechanism
With this command configured, the device determines that a clock jump has occurred and pauses PTP synchronization if the clock is stable but the offset of the current sample exceeds threshold-value. The device uses the following rules to determine whether to synchronize the clock in the future:
·     Normal synchronization—If the offset of the next sample is equal to or smaller than threshold-value, PTP resumes time synchronization.
·     Pausing synchronization—If subsequent offsets remain greater than threshold-value, PTP stops time synchronization until the suppression count reaches the preset value. The device then determines that the master clock is stable. When the device receives the next PTP signal, the device synchronizes the time regardless of whether the offset value exceeds threshold-value.
As shown in Figure 10, assume that the values for suppression-count and threshold-value are set to 5 and 3, respectively. When the offset is less than or equal to 3, synchronization occurs. When a sudden clock change causes the offset to exceed 3, synchronization of the clock signal is stopped until with a maximum of suppression-count clock signals being paused for synchronization. At time points P0 through P5, the device does not perform time synchronization, because the offset value is greater than 3. At time point P6, the device performs time synchronization not whether the offset value exceeds threshold-value.
Figure 10 PTP clock source jump prevention
3.     Configure the PTP offset threshold and the number of times PTP time synchronization is suppressed.
ptp time-offset { suppression-count suppression-count | suppression-threshold threshold-value } *
By default, the PTP time offset threshold is 3000 nanoseconds and PTP time synchronization is suppressed twice.
Priorities for clocks are used to elect the GM. The smaller the priority value, the higher the priority.
3.     Configure the priority for the specified clock for GM election through BMC.
ptp priority clock-source local { priority1 priority1 | priority2 priority2 }
The default value varies by PTP profile:
¡     IEEE 1588 version 2, SMPTE ST 2059-2, or AES67-2015—The priority 1 and priority 2 values are both 128.
¡     IEEE 802.1AS—The priority 1 value is 246 and the priority 2 value is 248.
PTP logs help monitor the clock source status. The following PTP logs are available:
·     PTP log that indicates a lower time class
Each PTP clock source has a class value. For a ToD clock source, you can set its class value by using the ptp clock-source command. The higher the value, the lower the class. When the class value of the clock source crosses the class threshold, the system outputs a log for notification.
·     PTP log that indicates a higher time offset between the external reference clock and the PTP clock
If the device uses an external reference clock, it periodically calculates the time offset between the external reference clock and the PTP clock. When the offset exceeds the threshold, the device outputs a log for notification
·     PTP logs that indicate a higher time-offset-sum peak-to-peak value
The PTP module calculates the time-offset-sum peak-to-peak value at specific intervals and compares the value with the threshold configured by this command. If the value is larger than the threshold, the system outputs a log for notification.
·     PTP logs that indicate the time-locked or time-unlocked state
When the time offset of the PTP reference clock crosses the PTP time locking threshold, the PTP time is put into unlocked state. The system outputs a time-unlocked log for notification. When the time offset of the PTP reference clock drops to or below the PTP time locking threshold, the PTP time is put into locked state. The system outputs a time-locked log for notification.
2.     Configure the class threshold for the clock source.
ptp alarm-threshold clock-source-class class-value
By default, the class threshold for the clock source is 6.
Only the IEEE 1588 version 2 PTP profile supports this configuration.
3.     Configure the time-offset threshold between the external reference clock and the PTP clock.
ptp alarm-threshold time-offset time-offset-value
By default, the time-offset threshold is 500 ns between the external reference clock and the PTP clock.
4.     Set the time-offset-sum peak-to-peak threshold.
ptp alarm-threshold time-offset-sum pk-pk threshold-value
By default, the time-offset-sum peak-to-peak threshold is 500 ns.
5.     Set the PTP time locking and unlocking thresholds.
ptp alarm-threshold { time-lock lock-value | time-unlock unlock-value } *
By default, the PTP time locking threshold is 200 ns and unlocking threshold is 300 ns.
To get informed of important events of the PTP module, enable SNMP notification for the PTP module.
The notifications generated for the PTP module will be sent to the SNMP module of the device. Configure SNMP notification parameters for the notifications to be output as needed.
For information about SNMP and SNMP notifications, see SNMP configuration in Network Management and Monitoring Configuration Guide.
2.     Enable SNMP notification for the PTP module.
snmp-agent trap enable ptp
By default, SNMP notification is enabled for the PTP module.
Display PTP clock information.
display ptp clock [ all | instance ptp-instance-id ]
Display the delay correction history.
display ptp corrections [ all | instance ptp-instance-id ]
Display information about foreign master nodes.
display ptp foreign-masters-record [ interface interface-type interface-number ] [ all | instance ptp-instance-id ]
Display PTP information on an interface.
display ptp interface [ interface-type interface-number ] [ all | instance ptp-instance-id ]
Display brief PTP information on all interfaces.
display ptp interface brief
Display brief information about the PTP synchronization path from the GM to the device.
display ptp path-trace
Display parent node information for the PTP device.
display ptp parent [ all | instance ptp-instance-id ]
Display historical role change information for PTP ports.
display ptp port-history [ interface interface-type interface-number ] [ all | instance ptp-instance-id ]
Display PTP statistics.
display ptp statistics [ interface interface-type interface-number ] [ all | instance ptp-instance-id ]
Display PTP clock time properties.
display ptp time-property [ all | instance ptp-instance-id ]
Clear PTP statistics.
reset ptp statistics [ interface interface-type interface-number ] [ all | instance ptp-instance-id ]
As shown in Figure 11, configure PTP (IEEE 1588 version 2, IEEE 802.3/Ethernet transport, multicast transmission) to enable time synchronization between the devices.
·     Specify the IEEE 1588 version 2 PTP profile and the IEEE 802.3/Ethernet transport protocol for PTP messages on Device A, Device B, and Device C.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and E2ETC clock node type for Device B. All clock nodes elect a GM through BMC in the PTP domain.
·     Use the default Request_Response delay measurement mechanism on Device A and Device C.
Figure 11 Network diagram
Table 1 Interface label and interface name mappings
Interface label
Interface name
Interface1
Ten-GigabitEthernet1/0/1
Interface2
Ten-GigabitEthernet1/0/2
1.     Configure Device A:
# Specify the IEEE 1588 version 2 PTP profile.
[DeviceA] ptp profile 1588v2
# Specify the OC clock node type.
[DeviceA] ptp mode oc
# Create a PTP domain.
[DeviceA] ptp domain 0
# Enable PTP globally.
[DeviceA] ptp global enable
# Specify PTP for obtaining the time.
[DeviceA] clock protocol ptp
# Enable PTP on Ten-GigabitEthernet 1/0/1.
[DeviceA-Ten-GigabitEthernet1/0/1] ptp enable
2.     Configure Device B:
[DeviceB] ptp profile 1588v2
# Specify the E2ETC clock node type.
[DeviceB] ptp mode e2etc
[DeviceB] ptp domain 0
[DeviceB] ptp global enable
[DeviceB] clock protocol ptp
[DeviceB-Ten-GigabitEthernet1/0/1] ptp enable
# Enable PTP on Ten-GigabitEthernet 1/0/2.
[DeviceB] interface ten-gigabitethernet 1/0/2
[DeviceB-Ten-GigabitEthernet1/0/2] ptp enable
[DeviceB-Ten-GigabitEthernet1/0/2] quit
3.     Configure Device C:
<DeviceC> system-view
[DeviceC] ptp profile 1588v2
[DeviceC] ptp mode oc
[DeviceC] ptp domain 0
[DeviceC] ptp global enable
[DeviceC] clock protocol ptp
[DeviceC] interface ten-gigabitethernet 1/0/1
[DeviceC-Ten-GigabitEthernet1/0/1] ptp enable
[DeviceC-Ten-GigabitEthernet1/0/1] quit
When the network is stable, perform the following tasks:
·     Use the display ptp clock command to display PTP clock information.
·     Use the display ptp interface brief command to display brief PTP running information for all PTP interfaces.
# Display PTP clock information on Device A.
[DeviceA] display ptp clock
PTP global state    : Enabled
PTP profile         : IEEE 1588 Version 2
PTP mode            : OC
PTP whitelist state : Disabled
Slave only          : No
Lock status         : Unlocked
Clock ID            : 000FE2-FFFE-FF0000
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 1
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 65535
Offset from master : 0 (ns)
Mean path delay    : 0 (ns)
Steps removed      : 0
Local clock time   : Sun Jan 15 20:57:29 2019
# Display brief PTP running information for all PTP interfaces on Device A.
[DeviceA] display ptp interface brief
Name       InstID    State         Delay mechanism  Clock step  Asymmetry correction
XGE1/0/1   0         Master        E2E              Two         0
# Display PTP clock information on Device B.
[DeviceB] display ptp clock
PTP mode            : E2ETC
Slave only          : No
Clock ID            : 000FE2-FFFE-FF0001
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 2
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master  : N/A
Mean path delay     : N/A
Steps removed       : N/A
# Display brief PTP running information for all PTP interfaces on Device B.
[DeviceB] display ptp interface brief
XGE1/0/1   0         N/A           E2E              Two         0
XGE1/0/2   0         N/A           E2E              Two         0
The command outputs show that Device A is elected as the GM and Ten-GigabitEthernet1/0/1 on Device A is the master port.
Example: Configuring PTP (IEEE 1588 version 2, UDP transport, multicast transmission)
As shown in Figure 12, configure PTP (IEEE 1588 version 2, UDP transport, multicast transmission) to enable time synchronization between the devices.
·     Specify the IEEE 1588 version 2 PTP profile for Device A, Device B, and Device C.
·     Specify multicast UDP transport for PTP messages.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and P2PTC clock node type for Device B. All clock nodes elect a GM through BMC in the PTP domain.
·     Specify the peer delay measurement mechanism (p2p) for Device A and Device C.
Figure 12 Network diagram
Table 2 Interface label and interface name mappings
Interface label
Interface name
Interface1
Interface2
# Configure the source IP address for multicast PTP messages transmitted over UDP.
[DeviceA] ptp source 10.10.1.1
# On Ten-GigabitEthernet 1/0/1, specify the UDP transport protocol for PTP messages, specify the delay measurement mechanism as p2p, and enable PTP.
[DeviceA-Ten-GigabitEthernet1/0/1] ptp transport-protocol udp [DeviceA-Ten-GigabitEthernet1/0/1] ptp delay-mechanism p2p
# Specify the P2PTC clock node type.
[DeviceB] ptp mode p2ptc
[DeviceB] ptp source 10.10.2.1
# On Ten-GigabitEthernet 1/0/1, specify the UDP transport protocol for PTP messages and enable PTP.
DeviceB-Ten-GigabitEthernet1/0/1] ptp transport-protocol udp
# On Ten-GigabitEthernet 1/0/2, specify the UDP transport protocol for PTP messages and enable PTP.
[DeviceB-Ten-GigabitEthernet1/0/2] ptp transport-protocol udp
[DeviceC] ptp source 10.10.3.1
[DeviceC-Ten-GigabitEthernet1/0/1] ptp transport-protocol udp [DeviceC-Ten-GigabitEthernet1/0/1] ptp delay-mechanism p2p
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
XGE1/0/1   0         Master        P2P              Two         0
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed       : N/A
XGE1/0/1   0          N/A           P2P              Two         0
XGE1/0/2   0          N/A           P2P              Two         0
Example: Configuring multiple PTP instances (IEEE 1588 version 2, multicast transmission)
As shown in Figure 13, configure two PTP instances on a PTP network.
·     PTP instance 1: Assign Device A, Device B, and Device C to PTP instance 1.
¡     Specify the IEEE 1588 version 2 PTP profile and IEEE 802.3/Ethernet transport of PTP messages for the devices and assign the devices to PTP domain 1.
¡     Specify the OC clock node type for Device A and Device C and E2ETC clock node type for Device B. All these clock nodes elect a GM through BMC.
¡     Use the default Request_Response delay measurement mechanism on all clock nodes in PTP instance 1.
·     PTP instance 2: Assign Device D, Device B, and Device E to PTP instance 2.
¡     Specify the IEEE 1588 version 2 PTP profile and UDP transport of PTP messages for the devices and assign the devices to PTP domain 2.
¡     Specify the OC clock node type for Device D and Device E and P2PTC clock node type for Device B. All the clock nodes elect a GM through BMC.
¡     Use the peer delay measurement mechanism on Device D and Device E.
Figure 13 Network diagram
Table 3 Interface label and interface name mappings
Interface label
Interface name
Interface1
Interface2
Interface3
Ten-GigabitEthernet1/0/3
Interface4
Ten-GigabitEthernet1/0/4
1.     Configure PTP instance 1 (IEEE 802.3/Ethernet transport of PTP messages)
a.     Configure Device A:
# Create a PTP instance, specifying its ID as 1 and name as ptp1, and enter its view.
[DeviceA] ptp instance 1 name ptp1
[DeviceA-ptp-instance-1] ptp profile 1588v2
[DeviceA-ptp-instance-1] ptp mode oc
# Specify PTP domain 1.
[DeviceA-ptp-instance-1] ptp domain 1
[DeviceA-ptp-instance-1] quit
# Assign Ten-GigabitEthernet 1/0/1 to PTP instance 1, enter interface PTP instance view, and enable PTP.
[DeviceA-Ten-GigabitEthernet1/0/1] ptp instance 1
[DeviceA-Ten-GigabitEthernet1/0/1-ptp-instance-1] ptp enable
[DeviceA-Ten-GigabitEthernet1/0/1-ptp-instance-1] quit
b.     Configure Device B:
[DeviceB] ptp instance 1 name ptp1
[DeviceB-ptp-instance-1] ptp profile 1588v2
[DeviceB-ptp-instance-1] ptp mode e2etc
[DeviceB-ptp-instance-1] ptp domain 1
[DeviceB-ptp-instance-1] quit
[DeviceB-Ten-GigabitEthernet1/0/1] ptp instance 1
[DeviceB-Ten-GigabitEthernet1/0/1-ptp-instance-1] ptp enable
[DeviceB-Ten-GigabitEthernet1/0/1-ptp-instance-1] quit
# Assign Ten-GigabitEthernet 1/0/2 to PTP instance 1, enter interface PTP instance view, and enable PTP.
[DeviceB-Ten-GigabitEthernet1/0/2] ptp instance 1
[DeviceB-Ten-GigabitEthernet1/0/2-ptp-instance-1] ptp enable
[DeviceB-Ten-GigabitEthernet1/0/2-ptp-instance-1] quit
c.     Configure Device C:
[DeviceC] ptp instance 1 name ptp1
[DeviceC-ptp-instance-1]
[DeviceC-ptp-instance-1] ptp profile 1588v2
[DeviceC-ptp-instance-1] ptp mode oc
[DeviceC-ptp-instance-1] ptp domain 1
[DeviceC-ptp-instance-1] quit
[DeviceC-Ten-GigabitEthernet1/0/1] ptp instance 1
[DeviceC-Ten-GigabitEthernet1/0/1-ptp-instance-1] ptp enable
[DeviceC-Ten-GigabitEthernet1/0/1-ptp-instance-1] quit
2.     Configure PTP instance 2 (UDP transport of PTP messages)
a.     Configure Device D:
<DeviceD> system-view
[DeviceD] ptp global enable
# Create a PTP instance, specifying its ID as 2 and name as ptp2, and enter its view.
[DeviceD] ptp instance 2 name ptp2
[DeviceD-ptp-instance-2] ptp profile 1588v2
[DeviceD-ptp-instance-1] ptp mode oc
# Specify PTP domain 2.
[DeviceD-ptp-instance-2] ptp domain 2
# Specify the source IP address for multicast transmission of PTP messages over UDP.
[DeviceD-ptp-instance-2] ptp source 10.10.1.1
[DeviceD-ptp-instance-2] quit
[DeviceD] clock protocol ptp
# Assign Ten-GigabitEthernet1/0/1 to PTP instance 2 and enter interface PTP instance view. Specify UDP transport of PTP messages and the peer delay measurement mechanism and enable PTP.
[DeviceD] interface ten-gigabitethernet 1/0/1
[DeviceD-Ten-GigabitEthernet1/0/1] ptp instance 2
[DeviceD-Ten-GigabitEthernet1/0/1-ptp-instance-2] ptp transport-protocol udp
[DeviceD-Ten-GigabitEthernet1/0/1-ptp-instance-2] ptp delay-mechanism p2p
[DeviceD-Ten-GigabitEthernet1/0/1-ptp-instance-2] ptp enable
[DeviceD-Ten-GigabitEthernet1/0/1-ptp-instance-2] quit
[DeviceD-Ten-GigabitEthernet1/0/1] quit
[DeviceB] ptp instance 2 name ptp2
[DeviceB-ptp-instance-2] ptp profile 1588v2
[DeviceB-ptp-instance-2] ptp mode p2ptc
[DeviceB-ptp-instance-2] ptp domain 2
[DeviceB-ptp-instance-2] ptp source 10.10.2.1
[DeviceB-ptp-instance-2] quit
[DeviceB] clock protocol ptp mdc 1
# Assign Ten-GigabitEthernet 1/0/3 to PTP instance and enter interface PTP instance view. Specify UDP transport of PTP messages and enable PTP.
[DeviceB] interface ten-gigabitethernet 1/0/3
[DeviceB-Ten-GigabitEthernet1/0/3] ptp instance 2
[DeviceB-Ten-GigabitEthernet1/0/3-ptp-instance-2] ptp transport-protocol udp
[DeviceB-Ten-GigabitEthernet1/0/3-ptp-instance-2] ptp enable
[DeviceB-Ten-GigabitEthernet1/0/3-ptp-instance-2] quit
[DeviceB-Ten-GigabitEthernet1/0/3] quit
# Assign Ten-GigabitEthernet 1/0/4 to PTP instance and enter interface PTP instance view. Specify UDP transport of PTP messages and enable PTP.
[DeviceB] interface ten-gigabitethernet 1/0/4
[DeviceB-Ten-GigabitEthernet1/0/4] ptp instance 2
[DeviceB-Ten-GigabitEthernet1/0/4-ptp-instance-2] ptp transport-protocol udp
[DeviceB-Ten-GigabitEthernet1/0/4-ptp-instance-2] ptp enable
[DeviceB-Ten-GigabitEthernet1/0/4-ptp-instance-2] quit
[DeviceB-Ten-GigabitEthernet1/0/4] quit
c.     Configure Device E:
<DeviceE> system-view
[DeviceE] ptp global enable
[DeviceE] ptp instance 2 name ptp2
[DeviceE-ptp-instance-2] ptp profile 1588v2
[DeviceE-ptp-instance-2] ptp mode oc
[DeviceE-ptp-instance-2] ptp domain 2
[DeviceE-ptp-instance-2] ptp source 10.10.3.1
[DeviceE-ptp-instance-2] quit
[DeviceE] clock protocol ptp
# Assign Ten-GigabitEthernet 1/0/4 to PTP instance 2 and enter interface PTP instance view. Specify UDP transport of PTP messages and the peer delay measurement mechanism and enable PTP.
[DeviceE] interface ten-gigabitethernet 1/0/1
[DeviceE-Ten-GigabitEthernet1/0/1] ptp instance 2
[DeviceE-Ten-GigabitEthernet1/0/1-ptp-instance-2] ptp transport-protocol udp
[DeviceE-Ten-GigabitEthernet1/0/1-ptp-instance-2] ptp delay-mechanism p2p
[DeviceE-Ten-GigabitEthernet1/0/1-ptp-instance-2] ptp enable
[DeviceE-Ten-GigabitEthernet1/0/1-ptp-instance-2] quit
[DeviceE-Ten-GigabitEthernet1/0/1] quit
1.     Verify the configuration of PTP instance 1.
When the network is stable, perform the following tasks to verify the configuration of PTP instance 1.
¡     Use the display ptp clock command to display PTP clock information.
¡     Use the display ptp interface brief command to display brief PTP running information for all PTP interfaces.
# Display PTP clock information for PTP instance 1 on Device A.
[DeviceA] display ptp clock instance 1
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 1
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
Local clock time   : Tue Jul 23 09:41:50 2019
XGE1/0/1    1        Master        E2E              Two         0
# Display PTP clock information for PTP instance 1 on Device B.
[DeviceB] display ptp clock instance 1
PTP mode            : E2ETC
Slave only          : No
Clock type          : Local
Clock domain        : 1
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : N/A
XGE1/0/1   1         N/A           E2E              Two         0
XGE1/0/2   1         N/A           E2E              Two         0
XGE1/0/3   2         N/A           P2P              Two         0
XGE1/0/4   2         N/A           P2P              Two         0
The command output shows that Device A is elected as the GM, and Ten-GigabitEthernet1/0/1 on Device A sends time synchronization information to its downstreams as a master port.
2.     Verify the configuration of PTP instance 2.
When the network is stable, perform the following tasks to verify the configuration of PTP instance 2:
# Display PTP clock information for PTP instance 2 on Device D.
[DeviceD] display ptp clock instance 2
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 2
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
# Display brief PTP running information for all PTP interfaces on Device D.
[DeviceD] display ptp interface brief
XGE1/0/1   2          Master        P2P              Two         0
# Display PTP clock information for PTP instance 2 on Device B.
[DeviceB] display ptp clock instance 2
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 2
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : N/A
The command output shows that Device D is elected as the GM, and Ten-GigabitEthernet1/0/1 on Device D sends time synchronization information to its downstreams as a master port.
Example: Configuring PTP (IEEE 802.1AS, IEEE 802.3/Ethernet transport, multicast transmission)
As shown in Figure 14, configure PTP (IEEE 802.1AS, IEEE 802.3/Ethernet transport, multicast transmission) to enable time synchronization between Device A, Device B, and Device C.
·     Specify the IEEE 802.1AS PTP profile for Device A, Device B, and Device C.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and P2PTC clock node type for Device B. The clock nodes elect a GM through BMC in the PTP domain.
·     Use the default peer delay measurement mechanism on all clock nodes in the PTP domain.
Figure 14 Network diagram
Table 4 Interface label and interface name mappings
Interface label
Interface name
Interface1
Interface2
IMPORTANT
IMPORTANT:
The IEEE 802.1AS PTP profile transports PTP messages over IEEE 802.3/Ethernet rather than UDP in multicast rather than unicast mode.
# Specify the IEEE 802.1AS PTP profile.
[DeviceA] ptp profile 802.1AS
[DeviceB] ptp profile 802.1AS
# Specify the IEEE 1588 802.1AS PTP profile.
[DeviceC] ptp profile 802.1AS
PTP profile         : IEEE 802.1AS
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 246
Priority2     : 248
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 16640
Steps removed      : 0
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 246
Priority2     : 248
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed       : N/A
The command outputs show that Device A is elected as the GM, Ten-GigabitEthernet1/0/1 on Device A is the master port, and Device B has synchronized to Device A.
Example: Configuring PTP (SMPTE ST 2059-2, UDP transport, multicast transmission)
As shown in Figure 15, configure PTP (SMPTE ST 2059-2, UDP transport, multicast transmission) to enable time synchronization between Device A and Device C:
·     Specify the SMPTE ST 2059-2 PTP profile and multicast UDP transport of PTP messages for Device A, Device B, and Device C.
·     Specify the OC clock node type for Device A and Device C, and the P2PTC clock node type for Device B. All clock nodes elect a GM through BMC.
·     Use the peer delay measurement mechanism on all clock nodes in the PTP domain.
Figure 15 Network diagram
Table 5 Interface label and interface name mappings
Interface label
Interface name
Interface1
Interface2
IMPORTANT
IMPORTANT:
The SMPTE ST 2059-2 PTP profile transports PTP messages over UDP rather than IEEE 802.3/Ethernet. The profile supports both multicast and unicast transmission modes.
# Specify the SMPTE ST 2059-2 PTP profile.
[DeviceA] ptp profile st2059-2
# On Ten-GigabitEthernet 1/0/1, specify the peer delay measurement mechanism and enable PTP.
[DeviceB] ptp profile st2059-2
[DeviceC] ptp profile st2059-2
When the network is stable, perform the following tasks to verify the PTP configuration:
PTP profile         : SMPTE ST 2059-2
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master  : 106368539000 (ns)
Mean path delay     : 2791000 (ns)
Steps removed       : 1
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed       : N/A
The output shows that Device A is elected as the GM and Ten-GigabitEthernet1/0/1 on Device A sends time synchronization information to its downstreams as a master port.
Example: Configuring PTP (AES67-2015, UDP transport, multicast transmission)
As shown in Figure 16, configure PTP (AES67-2015, UDP transport, multicast transmission) to enable time synchronization between Device A and Device C:
·     Specify the AES67-2015 PTP profile and multicast UDP transport of PTP messages for Device A, Device B, and Device C.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and the P2PTC clock node type for Device B. All clock nodes elect a GM through BMC.
Figure 16 Network diagram
Table 6 Interface label and interface name mappings
Interface label
Interface name
Interface1
Interface2
IMPORTANT
IMPORTANT:
The AES67-2015 PTP profile transports PTP messages over UDP rather than IEEE 802.3/Ethernet. The profile supports both multicast and unicast transmission modes.
# Specify the AES67-2015 PTP profile.
[DeviceA] ptp profile aes67-2015
[DeviceB] ptp profile aes67-2015
[DeviceC] ptp profile aes67-2015
PTP profile         : AES67-2015
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed       : 1
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed       : N/A
