14-Network Management and Monitoring Command Reference
HomeSupportRoutersCR16000-M SeriesReference GuidesCommand ReferencesH3C CR16000-M Router Command Reference-R8630Pxx-6W10014-Network Management and Monitoring Command Reference
13-EAA commands
13-EAA commands 216.89 KB
EAA commands
action cli
Use action cli to add a CLI action to a monitor policy.
Use undo action to remove an action.
undo action number
A monitor policy does not contain any actions.
CLI-defined policy view
number: Specifies an action ID in the range of 0 to 231.
cli command-line: Specifies the command line to be executed when the event occurs. You can enter abbreviated forms of command keywords, but you must make sure the forms can uniquely identify the command keywords. For example, you can enter int loop 1 for the interface loopback 1 command.
You can configure a series of actions to be executed in response to the event specified in a monitor policy. EAA executes the actions in ascending order of action IDs. When you add actions to a policy, you must make sure the execution order is correct. If two actions have the same ID, the most recent one takes effect.
To execute a command in a view other than user view, you must define actions required for accessing the target view before defining the command execution action. In addition, you must number the actions in the order they should be executed, starting with entering system view.
For example, to shut down an interface, you must create the following actions in order:
1.     Action to enter system view.
2.     Action to enter interface view.
3.     Action to shut down the interface.
When you define an action, you can specify a value or specify a variable name for an argument. For more information about using EAA environment variables, see "rtm environment."
# Configure a CLI action for the CLI-defined policy test to shut down Ten-GigabitEthernet 3/0/1.
[Sysname] rtm cli-policy test
[Sysname-rtm-test] action 1 cli system-view
[Sysname-rtm-test] action 2 cli interface ten-gigabitethernet 3/0/1
[Sysname-rtm-test] action 3 cli shutdown
action reboot
Use action reboot to add a reboot action to a monitor policy.
action number reboot [ slot slot-number ]
undo action number
slot slot-number: Specifies a card by its slot number. If you do not specify a card, this command reboots the device.
The reboot action configured with this command reboots devices or cards without saving the running configuration. If you want to save the running configuration, use the action cli command to configure reboot actions.
# Specify an action of rebooting slot 1 for CLI-defined policy test.
[Sysname-rtm-test] action 3 reboot slot 1
action switchover
Use action switchover to add an active/standby switchover action to a monitor policy.
action number switchover
undo action number
This command does not trigger an active/standby MPU switchover in either of the following situations:
·     The device has only one MPU.
·     The standby MPU is not in up state.
# Configure an action for the CLI-defined policy test to perform an active/standby switchover.
[Sysname-rtm-test] action 3 switchover
action syslog
Use action syslog to add a Syslog action to a monitor policy.
undo action number
priority priority: Specifies the log severity level in the range of 0 to 7. A lower value represents a higher severity level.
facility local-number: Specifies a logging facility by its facility number in the range of local0 to local7. Facility numbers are used by a log host to identify log creation facilities for filtering log messages.
msg msg-body: Configures the log message body.
EAA sends log messages to the information center. You can configure the information center to output these messages to certain destinations. For more information about the information center, see "Configuring the information center."
# Configure an action for the CLI-defined policy test to send a log message "hello" with a severity of 7 from the facility device local3.
[Sysname-rtm-test] action 3 syslog priority 7 facility local3 msg hello
commit
Use commit to enable a CLI-defined monitor policy.
commit
No CLI-defined policies are enabled.
You must execute this command for a CLI-defined policy to take effect.
After changing the settings in a policy that has been enabled, you must re-execute this command for the changes to take effect.
# Enable CLI-defined policy test.
[Sysname-rtm-test] commit
display rtm environment
Use display rtm environment to display user-defined EAA environment variables and their values.
var-name: Specifies a user-defined EAA environment variable by its name, a case-sensitive string of 1 to 63 characters. The name can contain digits, letters, and the underscore sign (_), but its leading character cannot be the underscore sign. If you do not specify a variable, this command displays all user-defined EAA environment variables.
# Display all user-defined EAA environment variables.
<Sysname> display rtm environment
Name             Value
save_cmd         save main force
show_run_cmd     display current-configuration
Name
Name of a user-defined EAA environment variable. This field displays a maximum of 30 characters. To display a user-defined EAA environment variable name of more than 30 characters, use the display current-configuration command.
Value
Value of the user-defined EAA environment variable. This field displays a maximum of 30 characters. To display a user-defined EAA environment variable value of more than 30 characters, use the display current-configuration command.
display rtm policy
Use display rtm policy to display information about EAA monitor policies.
active: Specifies policies that are executing the actions.
verbose: Displays detailed information about monitor policies.
policy-name: Specifies a policy by its name, a case-sensitive string of 1 to 63 characters. If you do not specify a policy, the command displays information about all monitor policies.
To display the running configuration of CLI-defined monitor policies, execute the display current-configuration command in any view or execute the display this command in CLI-defined monitor policy view.
# Display monitor policies that are executing the actions.
<Sysname> display rtm policy active
JID   Type  Event      TimeActive           PolicyName
507   TCL   INTERFACE  Aug 29 14:55:55 2013 test
JID
Job ID, displayed only when you specify the active keyword.
Policy creation method:
·     TCL—The policy was configured by using Tcl.
·     CLI—The policy was configured from the CLI.
Event
Event type, including CLI, hotplug, interface, process, SNMP, SNMP-Notification, Syslog, and track.
TimeActive
Time when the monitor policy was triggered.
PolicyName
Name of the monitor policy.
# Display brief information about all created monitor policies.
Total number: 1
Type  Event      TimeRegistered       PolicyName
CLI              Aug 29 14:54:50 2013 test
Total number
Total number of the monitor policies.
Event
TimeRegistered
Time when the monitor policy was created.
PolicyName
# Display detailed information about all monitor policies.
<Sysname> display rtm policy registered verbose
  Total number: 1
   Policy Name: test
   Policy Type: CLI
    Event Type:
TimeRegistered: Aug 29 14:54:50 2013
     User-role: network-operator
Total number
Total number of the monitor polices.
PolicyName
Policy Type
Event Type
TimeRegistered
Time when the policy was created.
User-role
User roles for executing the monitor policy. To execute the monitor policy, an administrator must have a minimum of one of the displayed user roles.
event cli
Use event cli to configure a CLI event for a CLI-defined monitor policy.
Use undo event to delete the event in a CLI-defined monitor policy.
undo event
No CLI event is configured.
async [ skip ]: Enables or disables the system to execute the command that triggers the policy. If you specify the skip keyword, the system executes the actions in the policy without executing the command that triggers the policy. If you do not specify the skip keyword, the system executes both the actions in the policy and the command entered at the CLI.
sync: Enables the system to execute the command that triggers the event only if the policy has been executed successfully.
mode { execute | help | tab }: Specifies the CLI operation to monitor:
·     execute: Triggers the policy when a matching command is entered.
·     help: Triggers the policy when a question mark (?) is entered at a matching command line.
·     tab: Triggers the policy when the Tab key is pressed to complete a parameter in a matching command line.
pattern regular-exp: Specifies a regular expression for matching commands that trigger the policy. For more information about using regular expressions, see CLI in Fundamentals Configuration Guide.
Use CLI event monitor policies to monitor operations performed at the CLI.
You can configure only one event for a monitor policy. If the monitor policy already contains an event, the new event replaces the old event.
# Configure a CLI-defined policy to monitor execution of commands that contain the display interface brief string. Enable the system to execute the actions in the policy without executing the command that triggers the policy.
<Sysname>system-view
[Sysname-rmt-test] event cli async skip mode execute pattern display interface brief
# Configure a CLI-defined policy to monitor the use of the Tab key at command lines that contain the display interface brief string. Enable the system to execute the actions in the policy and display the complete parameter when Tab is pressed at a policy-matching command line.
[Sysname-rmt-test] event cli async mode tab pattern display interface brief
# Configure a CLI-defined policy to monitor the use of the question mark (?) at command lines that contain the display interface brief string. Enable the system to execute a policy-matching command line only if the actions in the policy are executed successfully when a question mark is entered at the command line.
[Sysname-rmt-test] event cli sync mode help pattern display interface brief
event hotplug
Use event hotplug to configure a hot-swapping event.
event hotplug [ insert | remove ] slot slot-number
undo event
No hotplug event is configured.
insert: Specifies the card insert event.
remove: Specifies the card remove event.
After you configure the event, the monitor policy is triggered when a card is inserted in or removed from the specified slot/subslot. If you do not specify the insert or remove keyword, EAA monitors the card slot for both insert and remove events.
You can configure only one event entry for a monitor policy. If the monitor policy already contains an event entry, the new event entry replaces the old event entry.
# Configure a CLI-defined policy to monitor the specified slot for card insert and remove events.
[Sysname-rtm-test] event hotplug slot 2
event interface
Use event interface to configure an interface event for a CLI-defined monitor policy.
event interface interface-type interface-number monitor-obj monitor-obj start-op start-op start-val start-val restart-op restart-op restart-val restart-val [ interval interval ]
undo event
No interface event is configured.
monitor-obj monitor-obj: Specifies the traffic statistic to be monitored on the interface. For keywords available for the monitor-obj argument, see Table 5.
start-op start-op: Specifies the operator for comparing the monitored traffic statistic with the start threshold. The start threshold is crossed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 6.
start-val start-val: Specifies the start threshold to be compared with the monitored traffic statistic. The value range is 0 to 4294967295.
restart-op restart-op: Specifies the operator for comparing the monitored traffic statistic with the restart threshold. The restart threshold is crossed if the comparison result meets the condition. For keywords available for the restart-op argument, see Table 6.
restart-val restart-val: Specifies the restart threshold to be compared with the monitored traffic statistic. The value range is 0 to 4294967295.
interval interval: Specifies the interval to sample the monitored traffic statistic for a comparison. The value range is 1 to 4294967295, in seconds. The default value is 300.
Table 5 Monitored objects
Monitored traffic statistic
input-drops
Number of discarded incoming packets during a sampling interval
input-errors
Number of incoming error packets during a sampling interval
output-drops
Number of discarded outgoing packets during a sampling interval
output-errors
Number of outgoing error packets during a sampling interval
rcv-bps
Receive rate, in bits per second
rcv-broadcasts
Number of incoming broadcasts during a sampling interval
rcv-kbps
Receive rate, in kilobits per second
rcv-kpps
Receive rate, in kilo packets per second
rcv-pps
Receive rate, in packets per second
tx-bps
Transmit rate, in bits per second
tx-kbps
Transmit rate, in kilobits per second
tx-kpps
Transmit rate, in kilo packets per second
tx-pps
Transmit rate, in packets per second
Table 6 Comparison operators
Comparison operator
eq
Equal to.
ge
Greater than or equal to.
gt
Greater than.
le
Less than or equal to.
lt
Less than.
ne
Not equal to.
Use interface event monitor policies to monitor traffic statistics on an interface.
EAA executes an interface event policy when the monitored interface traffic statistic crosses the start threshold in the following situations:
·     The statistic crosses the start threshold for the first time.
·     The statistic crosses the start threshold each time after it crosses the restart threshold.
The following is the interface event monitor process of EAA:
1.     Compares the traffic statistic sample with the start threshold at sampling intervals until the start threshold is crossed.
2.     Executes the policy.
3.     Compares the traffic statistic sample with the restart threshold at sampling intervals until the restart threshold is crossed.
4.     Compares the traffic statistic sample with the start threshold at sampling intervals until the start threshold is crossed.
5.     Executes the policy again.
This process cycles for the monitor policy to be executed and re-executed.
# Configure a CLI-defined policy to monitor the incoming error packet statistic on Ten-GigabitEthernet 3/0/1 every 60 seconds. Set the start threshold to 1000 and the restart threshold to 50. Enable EAA to execute the policy when the statistic exceeds 1000 for the first time. Enable EAA to re-execute the policy if the statistic exceeds 1000 each time after the statistic has dropped below 50.
[Sysname-rtm-test] event interface ten-gigabitethernet 3/0/1 monitor-obj input-errors start-op gt start-val 1000 restart-op lt restart-val 50 interval 60
event process
Use event process to configure a process event for a CLI-defined monitor policy.
event process { exception | recover-failure | restart | shutdown | start } [ name process-name [ instance instance-id ] ] [ slot slot-number ]
undo event
No process event is configured.
exception: Monitors the specified process for exceptional events. EAA executes the policy when an exception occurs to the monitored process.
recover-failure: Monitors the specified process for recovery failure events. EAA executes the policy when the monitored process fails to recover from an anomaly.
restart: Monitors the specified process for restart events. EAA executes the policy when the monitored process restarts.
shutdown: Monitors the specified process for shutdown events. EAA executes the policy when the monitored process is shut down.
start: Monitors the specified process for start events. EAA executes the policy when the monitored process starts.
name process-name: Specifies a user-mode process by its name. The process can be one that is running or not running. If you do not specify a name, this command monitors all use-mode processes.
instance instance-id: Specifies a process instance ID in the range of 0 to 4294967295. The instance ID can be one that has not been created yet. If you do not specify an instance, EAA monitors all instances of the process.
slot slot-number: Specifies a card by its slot number. If you do not specify a card, this command applies to the device.
Use process event monitor policies to monitor process state changes. These changes can result from manual operations or automatic system operations.
# Configure a CLI-defined policy to monitor all instances of the process snmpd for restart events.
[Sysname-rtm-test] event process restart name snmpd
event snmp oid
Use event snmp oid to configure an SNMP event for a CLI-defined monitor policy.
undo event
No SNMP event is configured.
oid oid: Specifies the OID of the monitored MIB variable, a string of 1 to 256 characters.
monitor-obj { get | next }: Specifies the SNMP operation used for sampling variable values. The get keyword represents the SNMP get operation, and the next keyword represents the SNMP getNext operation.
start-op start-op: Specifies the operator for comparing the sampled value with the start threshold. The start threshold is crossed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 7.
start-val start-val: Specifies the start threshold to be compared with the sampled value. The start-val argument can be any data type supported by SNMP, including numerals and character strings. The  value range for the start-val argument is a string of 1 to 512 characters. If the threshold value contains spaces, you must enclose the value in quotation marks (" ").
restart-op op: Specifies the operator for comparing the sampled value with the restart threshold. The restart threshold is crossed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 7.
restart-op restart-val: Specifies the restart threshold to be compared with the sampled value. The restart-val argument can be any data type supported by SNMP, including numerals and character strings. The value range for the restart-val argument is a string of 1 to 512 characters. If the threshold value contains spaces, you must enclose the value in quotation marks (" ").
interval interval: Specifies the sampling interval in the range of 1 to 4294967295, in seconds. The default value is 300.
Table 7 Comparison operators
Comparison operator
eq
Equal to.
ge
gt
Greater than.
le
lt
Less than.
ne
Not equal to.
Use SNMP event monitor policy to monitor value changes of MIB variables.
EAA executes an SNMP event policy when the monitored MIB variable's value crosses the start threshold in the following situations:
·     The monitored variable's value crosses the start threshold for the first time.
·     The monitored variable's value crosses the start threshold each time after it crosses the restart threshold.
The following is the SNMP event monitor process of EAA:
1.     Compares the variable sample with the start threshold at sampling intervals until the start threshold is crossed.
3.     Compares the variable sample with the restart threshold at sampling intervals until the restart threshold is crossed.
4.     Compares the variable sample with the start threshold at sampling intervals until the start threshold is crossed.
# Configure a CLI-defined policy to get the value of the MIB variable 1.3.6.4.9.9.42.1.2.1.6.4 every five seconds. Set the start threshold to 1 and the restart threshold to 2. Enable EAA to execute the policy when the value changes to 1 for the first time. Enable EAA to re-execute the policy if the value changes to 1 each time after the value has changed to 2.
[Sysname-rtm-test] event snmp oid 1.3.6.4.9.9.42.1.2.1.6.4 monitor-obj get start-op eq start-val 1 restart-op eq restart-val 2 interval 5
event snmp-notification
Use event snmp-notification to configure an SNMP-Notification event for a CLI-defined policy.
Use undo event to remove the event in a CLI-defined policy.
undo event
No SNMP-Notification event is configured.
oid-val oid-val: Specifies the threshold to be compared with the sampled value. The oid-val argument can be any data type supported by SNMP, including numerals and character strings. The value range for the oid-val argument is a string of 1 to 512 characters. If the threshold value contains spaces, you must enclose the value in quotation marks (" ").
op op: Specifies the operator for comparing the sampled value with the threshold. The policy is executed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 8.
drop: Drops the notification if the comparison result meets the condition. If you do not specify this keyword, the system sends the notification.
Table 8 Comparison operators
Comparison operator
eq
Equal to.
ge
gt
Greater than.
le
lt
Less than.
ne
Not equal to.
Use SNMP-Notification event monitor policies to monitor variables in SNMP notifications.
EAA executes an SNMP-Notification event monitor policy when the value of the monitored variable in an SNMP notification meets the specified condition.
# Configure a CLI-defined policy to monitor SNMP notifications that contain the use name variable 1.3.6.1.4.1.25506.2.2.1.1.2.1.0. Enable the system to execute the policy and drop the SNMP notification if the use name variable value is admin.
[Sysname-rtm-test] event snmp-notification oid 1.3.6.1.4.1.25506.2.2.1.1.2.1.0 oid-val admin op eq drop
event syslog
Use event syslog to configure a Syslog event for a CLI-defined monitor policy.
event syslog priority { priority | all }msg msg occurs times period period
undo event
No Syslog event is configured.
priority { priority | all }: Specifies the severity level for matching log messages.
·     priority specifies the lowest severity level for matching log messages. The value is an integer in the range of 0 to 7. A lower number represents higher severity level. For example, specify a severity level of 3 to match log messages from level 3 to level 0.
·     All represents all severity levels.
msg msg: Specifies a regular expression to match the log message body. The msg argument represents a regular expression, a string of 1 to 255 characters.
occurs times period period: Executes the policy if the number of log matches over an interval exceeds the limit. The times argument specifies the maximum number of log matches in the range of 1 to 32. The period argument specifies an interval in the range of 1 to 4294967295 seconds.
Use Syslog event monitor policies to monitor log messages.
EAA executes a Syslog event monitor policy when the number of matching logs over an interval reaches the limit.
EAA does not count log messages generated by the RTM module when it counts log matches.
A regular expression can contain the special characters described in Table 9.
Table 9 Special characters supported in a regular expression
Characters
Meaning
Matches the beginning of a line.
"^u" matches all lines beginning with "u". A line beginning with "Au" is not matched.
Matches the end of a line.
"u$" matches all lines ending with "u". A line ending with "uA" is not matched.
. (period)
Matches any single character.
".s" matches "as" and "bs".
Matches the preceding character or string zero, one, or multiple times.
"zo*" matches "z" and "zoo", and "(zo)*" matches "zo" and "zozo".
Matches the preceding character or string one or multiple times.
"zo+" matches "zo" and "zoo", but not "z".
Matches the preceding or succeeding string.
"def|int" matches a line containing "def" or "int".
Matches the string in the parentheses, usually used together with the plus sign (+) or asterisk sign (*).
"(123A)" matches "123A".
"408(12)+" matches "40812" and "408121212", but not "408".
\N
Matches the preceding strings in parentheses, with the Nth string repeated once.
"(string)\1" matches a string containing "stringstring".
"(string1)(string2)\2" matches a string containing "string1string2string2".
"(string1)(string2)\1\2" matches a string containing " string1string2string1string2".
Matches a single character in the brackets.
"[16A]" matches a string containing 1, 6, or A; "[1-36A]" matches a string containing 1, 2, 3, 6, or A (- is a hyphen).
To match the character "]", put it immediately after "[", for example, []abc]. There is no such limit on "[".
Matches a single character that is not in the brackets.
"[^16A]" matches a string that contains one or more characters except for 1, 6, or A, such as "abc". A match can also contain 1, 6, or A (such as "m16"), but it cannot contain these three characters only (such as 1, 16, or 16A).
{n}
Matches the preceding character n times. The number n must be a nonnegative integer.
"o{2}" matches "food", but not "Bob".
{n,}
Matches the preceding character n times or more. The number n must be a nonnegative integer.
"o{2,}" matches "foooood", but not "Bob".
{n,m}
Matches the preceding character n to m times or more. The numbers n and m must be nonnegative integers and n cannot be greater than m.
" o{1,3}" matches "fod", "food", and "foooood", but not "fd".
Matches a string that starts with the pattern following \<. A string that contains the pattern is also a match if the characters preceding the pattern are not digits, letters, or underscores.
"\<do" matches "domain" and "doa".
Matches a string that ends with the pattern preceding \>. A string that contains the pattern is also a match if the characters following the pattern are not digits, letters, or underscores.
"do\>" matches "undo" and "cdo".
\b
Matches a word that starts with the pattern following \b or ends with the pattern preceding \b.
"er\b" matches "never", but not "verb" or "erase".
"\ber" matches "erase", but not "verb" or "never".
\B
Matches a word that contains the pattern but does not start or end with the pattern.
"er\B" matches "verb", but not "never" or "erase".
\w
Same as [A-Za-z0-9_], matches a digit, letter, or underscore.
"v\w" matches "vlan" and "service".
\W
Same as [^A-Za-z0-9_], matches a character that is not a digit, letter, or underscore.
"\Wa" matches "-a", but not "2a" or "ba".
Escape character. If a special character listed in this table follows \, the specific meaning of the character is removed.
"\\" matches a string containing "\", "\^" matches a string containing "^", and "\\b" matches a string containing "\b".
# Configure a CLI-defined policy to monitor Syslog messages for level 3 to level 0 messages that contain the down string. Enable the policy to execute when five log matches are found within 6 seconds.
[Sysname-rtm-test] event syslog priority 3 msg down occurs 5 period 6
event track
Use event track to configure a track event for a CLI-defined monitor policy.
undo event
A CLI-defined policy does not contain a track event.
track-list: Specifies a space-separated list of up to 16 track items. Each item specifies a track entry number or a range of track entry numbers in the form of track-entry-number to track-entry-number. The value range for the track-entry-number argument is 1 to 1024.
state { negative | positive }: Monitors state change of the track entries.
·     negative: Triggers the policy when the states of the track entries change from Positive to Negative.
·     positive: Triggers the policy when the state of the track entries change from Negative to Positive.
suppress-time suppress-time: Sets a suppress time in the range of 1 to 4294967295, in seconds. The default value is 0.
After you configure a track event for an EAA monitor policy, the track event occurs and triggers the policy when the state of the track entry changes from Positive to Negative or from Negative to Positive. If you specify multiple track entries for a policy, the policy is triggered only when the state of all the track entries changes from Positive to Negative or Negative to Positive.
For example, for the sessions between the local device and its downlink BGP peers to disconnect automatically when the sessions between the local device and its uplink BGP peers are disconnected, you can configure a track event monitor policy as follows:
·     Configure a track event for the policy and specify track entries to monitor the links between the local device and its uplink BGP peers.
·     Add the CLI action peer ignore to the policy to disable BGP session establishment between the local device and its downlink BGP peers.
To avoid frequent triggering of the EAA monitor policy by the track event, you can specify suppression time to control the interval between executions of the monitor policy. After the suppression time is configured, the policy is triggered and the suppression timer is started when the track event occurs for the first time.
·     If the track event occurs again before or when the suppression timer expires, the track event will be suppressed and will not trigger the monitor policy.
·     If the track event occurs again after the suppression timer expires, the monitor policy is triggered and the suppression timer will be reset and restart timing until the monitor policy is stopped.
For example, if you execute the track 1 interface gigabiteethernet 1/0/1 and event track 1 state negative suppress-time 60 commands to configure a track event for a monitor policy, the following occurs:
·     When the state of interface Ten-GigabitEthernet 3/0/1 changes to down for the first time, the monitor policy is triggered.
·     If the state of interface Ten-GigabitEthernet 3/0/1 changes to down again within 60 seconds, the monitor policy will not be triggered. This prevents frequent triggering of the monitor policy within one minute in case of state flapping of Ten-GigabitEthernet 3/0/1.
·     If the state of interface Ten-GigabitEthernet 3/0/1 changes to down again after 1 minute, the monitor policy is triggered.
# Create the CLI-defined monitor policy test. Configure a track event for the policy that occurs when the states of track entry 1 to track entry 8 change from Positive to Negative. Set the suppress time to 180 seconds for the policy. Configure an action for the policy that disconnects the session between the device and its BGP peer.
[Sysname-rtm-test] event track 1 to 8 state negative suppress-time 180
[Sysname-rtm-test] action 0 cli system-view
[Sysname-rtm-test] action 1 cli bgp 100
[Sysname-rtm-test] action 2 cli peer 10.1.1.1 ignore
rtm cli-policy
Use rtm cli-policy to create a CLI-defined EAA monitor policy and enter its view, or enter the view of an existing CLI-defined EAA monitor policy.
Use undo rtm cli-policy to delete a CLI-defined monitor policy.
rtm cli-policy policy-name
undo rtm cli-policy policy-name
No CLI-defined monitor policies exist.
policy-name: Specifies the name of a CLI-defined monitor policy, a case-sensitive string of 1 to 63 characters.
You must create a CLI-defined monitor policy before you can use the CLI to configure settings in the policy.
For a CLI-defined monitor policy to take effect, you must execute the commit command after you complete configuring the policy.
You can execute this command multiple times to create multiple CLI-defined monitor policies. Make sure the CLI-defined monitor policies that are executed at the same time do not have conflicting actions. If the actions conflict, the system executes the actions randomly.
You can assign the same name to a CLI-defined policy and a Tcl-defined policy.
# Create a CLI-defined policy and enter its view.
commit
rtm environment
Use rtm environment to configure an EAA environment variable.
Use undo rtm environment to delete a user-defined EAA environment variable.
undo rtm environment var-name
No user-defined EAA environment variables exist.
The system provides the variables in Table 10. You cannot create, delete, or modify these system-defined variables.
Table 10 System-defined EAA environment variables by event type
Event
Variable name and description
Any event
_event_id: Event ID
_event_type: Event type
_event_type_string: Event type description
_event_time: Time when the event occurs
_event_severity: Severity level of an event
CLI
_cmd: Commands that are matched
Syslog
_syslog_pattern: Log message content
Hotplug
_slot: ID of the slot where card hot-swapping occurs
_ifname: Interface name
SNMP
_oid: OID of the MIB variable where an SNMP operation is performed
_oid_value: Value of the MIB variable
SNMP-Notification
_oid: OID that is included in the SNMP notification.
Process
_process_name: Process name
var-value: Specifies the variable value.
When you define an action, you can enter a variable name with a leading dollar sign ($variable_name) instead of entering a value for an argument. EAA will replace the variable name with the variable value when it performs the action.
For an action argument, you can specify a list of variable names in the form of $variable_name1$variable_name2...$variable_nameN.
# Create an environment variable: set its name to if and set its value to interface.
[Sysname] rtm environment if interface
rtm event syslog buffer-size
Use rtm event syslog buffer-size to set the size for the EAA-monitored log buffer.
Use undo rtm event syslog buffer-size to restore the default.
The EAA-monitored log buffer can store a maximum of 50000 logs.
buffer-size: Specifies the size for the EAA-monitored log buffer. The value range for this argument is 1 to 500000.
After you execute a Syslog event monitor policy, the system saves a copy of the logs to the EAA-monitored log buffer. When the logs in the buffer match the Syslog event, EAA executes the monitor policy actions.
Typically, the default EAA-monitored log buffer size is sufficient. However, when a feature malfunctions or the user enables multiple debugging functions, a large number of logs are generated. Some logs might be discarded before the matching is performed. You can set the EAA-monitored log buffer to a large size based on the memory usage.
# Set the size of the EAA-monitored log buffer to 1000.
[Sysname] rtm event syslog buffer-size 1000
event syslog
rtm scheduler suspend
Use rtm scheduler suspend to suspend monitor policies.
Use undo rtm scheduler suspend to resume monitor policies.
You need to suspend the monitor policies under the following circumstances:
·     The monitor policies are triggered frequently, affecting the system services and performance.
·     The Tcl script of a policy needs to be revised.
After you execute this command, EAA will not execute the policies even if the trigger conditions are met.
This command does not suspend a running monitor policy until all its actions are executed.
# Suspend monitor policies.
[Sysname] rtm scheduler suspend
rtm tcl-policy
Use rtm tcl-policy to create a Tcl-defined policy and bind it to a Tcl script file.
Use undo rtm tcl-policy to delete a Tcl policy.
undo rtm tcl-policy policy-name
No Tcl policies exist.
policy-name: Specifies a policy name, a case-sensitive string of 1 to 63 characters.
tcl-filename: Specifies a .tcl script file name. The file name is case sensitive. You must ensure that the file is available on a storage medium of the device.
When you use this command to create a Tcl-defined policy, follow these guidelines:
Make sure the script file is saved on all MPUs. This practice ensures that the policy can run correctly after an active/standby or master/standby switchover occurs or the MPU where the script file resides fails or is removed.
This command both creates and enables the specified Tcl-defined monitor policy. To revise the Tcl script of a Tcl-defined policy, you must suspend all monitor policies first, and then resume the policies after you finish revising the script. The system cannot execute a Tcl-defined policy if you edit its Tcl script without suspending all monitor policies.
To bind a Tcl-defined policy to a different Tcl script file:
1.     Execute the undo rtm tcl-policy command to delete the Tcl policy.
2.     Create the Tcl policy again, and then bind it to the new Tcl script file.
You can assign the same policy name to a CLI-defined policy and a Tcl-defined policy. However, you cannot assign the same name to policies that are the same type.
# Create a Tcl policy and bind it to a Tcl script file.
[Sysname] rtm tcl-policy test test.tcl
running-time
Use running-time to configure the action runtime of a CLI-defined policy.
Use undo running-time to restore the default.
running-time time
undo running-time
The action runtime of a CLI-defined policy is 20 seconds.
time: Specifies the action runtime in the range of 0 to 31536000 seconds. If you specify 0, the policy runs its actions forever once the policy is triggered.
The action runtime limits the amount of time that the monitor policy runs its actions from the time it is triggered. When the runtime is reached, the system stops executing the policy even if the execution is not finished.
This setting prevents a policy from running its actions permanently to occupy resources.
# Set the action runtime to 60 seconds for CLI-defined policy test.
[Sysname-rtm-test] running-time 60
user-role
Use user-role to assign a user role to a CLI-defined policy.
Use undo user-role to remove a user role from a CLI-defined policy.
user-role role-name
undo user-role role-name
A monitor policy contains user roles that its creator had at the time of policy creation.
role-name: Specifies a user role by its name, a case-sensitive string of 1 to 63 characters. You can specify an existing user role in the device, such as network-admin or network-operator. When you execute the user-role ? command in CLI-defined policy view, the device displays the names of the existing user roles. You can also specify a non-existent user role. If the specified user role name does not exist on the device, you must create the user by using the role name role-name command and configure permissions for it. For more information about user role configuration, see Fundamentals Configuration Guide.
For EAA to execute an action in a monitor policy, you must assign the policy the user role that has access to the action-specific commands and resources. If EAA lacks access to an action-specific command or resource, EAA does not perform the action and all the subsequent actions.
For example, a monitor policy has four actions numbered from 1 to 4. The policy has user roles that are required for performing actions 1, 3, and 4, but it does not have the user role required for performing action 2. When the policy is triggered, EAA executes only action 1.
A monitor policy supports a maximum of 64 valid user roles. User roles added after this limit is reached do not take effect.
An EAA policy cannot have both the security-audit user role and any other user roles. Any previously assigned user roles are automatically removed when you assign the security-audit user role to the policy. The previously assigned security-audit user role is automatically removed when you assign any other user roles to the policy.
# Assign user roles to a CLI-defined policy.
[Sysname-rtm-test] user-role admin