17-Network Management and Monitoring Command Reference
HomeSupportReference GuidesCommand ReferencesH3C SecPath M9000 Command Reference(V7)(R9X71)-6W70117-Network Management and Monitoring Command Reference
11-Event MIB commands
11-Event MIB commands 279.80 KB
Event MIB commands
action
Use action to set an action for an event.
Use undo action to remove an action.
action { notification | set }
undo action { notification | set }
An event does not have an action.
Event view
context-admin
notification: Specifies the notification action. The system sends a notification to the NMS when the event is triggered.
set: Specifies the set action. The system sets a value for the specified MIB object when the event is triggered.
You can set both set and notification actions for an event.
·     When you specify the set action, the system automatically creates a set entry and enters action-set view. You can configure the set action in this view. For more information, see the configuration in action-set view.
·     When you specify the notification action, the system automatically creates a notification entry and enters action-notification view. You can configure the notification action in this view. For more information, see the configuration in action-notification view.
# Set the notification action for an event and specify notification OID mteEventSetFailure for the action. Set the set action for the event and set the value for the ipForwarding.0 object to 2.
[Sysname] snmp mib event owner owner1 name EventA
[Sysname-event-owner1-EventA] action notification
[Sysname-event-owner1-EventA-notification] oid mteEventSetFailure
[Sysname-event-owner1-EventA-notification] quit
[Sysname-event-owner1-EventA] action set
[Sysname-event-owner1-EventA-set] oid ipForwarding.0
[Sysname-event-owner1-EventA-set] value 2
event enable
snmp mib event
comparison
Use comparison to specify a Boolean comparison type for the sampled value and the reference value.
Use undo comparison to restore the default.
comparison { equal | greater | greaterorequal | less | lessorequal | unequal }
undo comparison
The Boolean comparison type is unequal.
Trigger-Boolean view
context-admin
equal: Specifies the Boolean comparison type as equal. When the sampled value equals the reference value, the trigger condition is met.
greater: Specifies the Boolean comparison type as greater than. When the sampled value is greater than the reference value, the trigger condition is met.
greaterorequal: Specifies the Boolean comparison type as greater than or equal to. When the sampled value is greater than or equal to the reference value, the trigger condition is met.
less: Specifies the Boolean comparison type as smaller than. When the sampled value is smaller than the reference value, the trigger condition is met.
lessorequal: Specifies the Boolean comparison type as smaller than or equal to. When the sampled value is smaller than or equal to the reference value, the trigger condition is met.
unequal: Specifies the Boolean comparison type as unequal. When the sampled value is unequal to the reference value, the trigger condition is met.
If the sampled value meets the trigger condition at two or more samplings in succession, an event is triggered only at the first sampling.
For an event to be triggered at the first sampling, execute the startup enable command.
# Specify the Boolean comparison type as unequal.
[Sysname] snmp mib event trigger owner owner1 name triggerA
[Sysname-trigger-owner1-triggerA] test boolean
[Sysname-trigger-owner1-triggerA-boolean] comparison unequal
test
context (action-set view)
Use context to configure a context for the set-action object.
Use undo context to restore the default.
context context-name
undo context
A set-action object does not have a context.
Action-set view
context-admin
context-name: Specifies a context, a case-sensitive string of 1 to 32 characters.
To uniquely identify a set-action object, configure a context for it.
# Configure context contextname1 for the set-action object.
<Sysname>system-view
[Sysname-event-owner1-EventA-set] context contextname1
action
wildcard context
context (trigger view)
Use context to configure a context for a monitored object.
undo context
A monitored object does not have a context.
Trigger view
context-admin
To uniquely identify a monitored object, configure a context for it.
# Configure context contextname1 for a monitored object.
[Sysname-trigger-owner1-triggerA] context contextname1
wildcard context
delta falling
Use delta falling to set a delta falling threshold and specify a falling event.
Use undo delta falling to restore the default.
delta falling { event owner event-owner name event-name | value integer-value }
undo delta falling { event | value }
The delta falling threshold is 0, and no falling event is specified.
Trigger-threshold view
context-admin
event owner event-owner name event-name: Specifies an event by its owner and its name. Use the trigger owner as the event owner. The event-name argument is a case-sensitive string of 1 to 32 characters.
value integer-value: Specifies a delta falling threshold in the range of –2147483648 to 2147483647. The value must be smaller than or equal to the delta rising threshold.
A falling event is triggered if the delta value (difference between the current sampled value and the previous sampled value) is smaller than or equal to the delta falling threshold.
If the delta value crosses the delta falling threshold multiple times in succession, a falling event is triggered only for the first crossing.
# Set the delta falling threshold to 20.
[Sysname-trigger-owner1-triggerA] test threshold
[Sysname-trigger-owner1-triggerA-threshold] delta falling value 20
sample
test
delta rising
Use delta rising to set a delta rising threshold and specify a rising event.
Use undo delta rising to restore the default.
delta rising { event owner event-owner name event-name | value integer-value }
undo delta rising { event | value }
The delta rising threshold is 0, and no rising event is specified.
context-admin
value integer-value: Specifies a delta rising threshold in the range of –2147483648 to 2147483647. The value must be greater than or equal to the delta falling threshold.
A rising event is triggered if the delta value is greater than or equal to the delta rising threshold.
If the delta value of the monitored object crosses the delta rising threshold multiple times in succession, a rising event is triggered only for the first crossing.
# Set the delta rising threshold to 50, and specify the event identified by owner owner1 and name event1 as the rising event.
[Sysname-trigger-owner1-triggerA-threshold] delta rising value 50
[Sysname-trigger-owner1-triggerA-threshold] delta rising event owner owner1 name event1
sample
test
description (event view)
Use description to configure a description for an event.
An event does not have a description.
Event view
context-admin
# Configure a description of EventA is an RMON event for the event identified by owner owner1 and name eventA.
[Sysname-event-owner1-EventA] description EventA is an RMON event
description (trigger view)
Use description to configure a description for a trigger.
A trigger does not have a description.
Trigger view
context-admin
# Configure a description of triggerA is configured for configured for network management events for the trigger identified by owner owner1 and name triggerA.
[Sysname-trigger-owner1-triggerA] description triggerA is configured for network management events
display snmp mib event
Use display snmp mib event to display Event MIB configuration and statistics.
context-admin
context-operator
# Display Event MIB configuration and statistics.
<Sysname> display snmp mib event
TriggerFailures               : 0
EventFailures                 : 0
SampleMinimum                 : 1
SampleInstanceMaximum         : 0
SampleInstance                : 0
SampleInstancesHigh           : 0
SampleInstanceLacks           : 0
Trigger entry triggerA owned by owner1:
  TriggerComment              : triggerA is to monitor the state of the interface
  TriggerTest                 : boolean
  TriggerSampleType           : absoluteValue
  TriggerValueID              : 1.3.6.1.2.1.2.2.1.7.3<ifAdminStatus.3>
  TriggerValueIDWildcard      : false
  TriggerTargetTag            : N/A
  TriggerContextName          : context1
  TriggerContextNameWildcard  : true
  TriggerFrequency(in seconds): 600
  TriggerEnabled              : true
  Boolean entry:
   BoolCmp                    : unequal
   BoolValue                  : 1
   BoolStartUp                : true
   BoolObjOwner               : owner1
   BoolObjName                : Objects1
   BoolEvtOwner               : N/A
   BoolEvtName                : N/A
Event entry eventA owned by owner2:
  EvtComment                  : event is to set ifAdminStatus
  EvtAction                   : notification | set
  EvtEnabled                  : true
  Notification entry:
   NotifyOID                  : 1.3.6.1.2.1.88.2.0.1<mteTriggerFired>
   NotifyObjOwner             : N/A
   NotifyObjName              : N/A
  Set entry:
   SetObj                     : 1.3.6.1.2.1.2.2.1.7<ifAdminStatus>
   SetObjWildcard             : true
   SetValue                   : 2
   SetTargetTag               : N/A
   SetContextName             : context1
   SetContextNameWildcard     : false
Object list objectA owned by owner3:
  ObjIndex                    : 1
  ObjID                       : 1.3.6.1.2.1.2.1.0<ifNumber.0>
  ObjIDWildcard               : false
  ObjIndex                    : 2
  ObjID                       : 1.3.6.1.2.1.2.2.1.2.0<ifDescr.0>
For more information about the command output, see Table 1 to Table 4.
snmp mib event
snmp mib event object list
display snmp mib event event
Use display snmp mib event event to display information about an event and the event actions.
display snmp mib event event [ owner event-owner name event-name ]
context-admin
context-operator
owner event-owner name event-name: Specifies an event by its owner and name. The event-owner argument must be an existing SNMPv3 user.  The event-name argument is a case-sensitive string of 1 to 32 characters. If you do not specify an event, this command displays information about all events and event actions.
# Display information about the event identified by owner owner2 and name eventA and the event actions.
<Sysname>display snmp mib event event owner owner2 name eventA
  EvtEnabled                  : true
  Notification entry:
   NotifyObjName              : N/A
  Set entry:
   SetValue                   : 2
   SetTargetTag               : N/A
Event entry
EvtComment
Description for the event.
EvtAction
Event actions:
·     Set action.
·     Notification action.
EvtEnabled
Event status:
·     Enabled.
·     Disabled.
Notification entry
NotifyOID
Notification OID.
NotifyObjOwner
Owner of the notification-action object.
NotifyObjName
Name of the object list to be added to the notification.
Set entry
SetObj
OID of the set-action object.
SetObjWildcard
Wildcarding option for the OID:
·     false—Specifies an object by its OID.
·     true—Enables a wildcard search for OIDs.
SetValue
Value of the set-action object.
SetTargetTag
Remote tag for the set-action object.
SetContextName
Context for the set-action object.
Wildcarding option for the context
·     false—Specifies a context.
·     true—Enables wildcard search for contexts.
snmp mib event
display snmp mib event object list
Use display snmp mib event event to display information about object lists.
display snmp mib event object list [ owner group-owner name group-name ]
context-admin
context-operator
owner group-owner name group-name: Specifies an object list by its owner and name. The objects -owner argument must be an existing SNMPv3 user. The objects name argument is a case-sensitive string of 1 to 32 characters. If you do not specify an object list, this command displays information about all object lists.
# Display information about the object list identified by owner owner3 and name objectA.
<Sysname> display snmp mib event object list owner owner3 name objectA
ObjIndex                    : 1
ObjIndex                    : 2
ObjIndex
Index of the object.
ObjID
OID of the object.
ObjIDWildcard
·     false—Specifies the OID.
·     true—Enables wildcard search for OIDs.
display snmp mib event summary
Use display snmp mib event summary to display Event MIB brief information.
context-admin
context-operator
# Display Event MIB brief information.
<Sysname> display snmp mib event summary
TriggerFailures               : 0
EventFailures                 : 0
SampleMinimum                 : 1
SampleInstance                : 0
TriggerFailures
Number of trigger test failures.
EventFailures
Number of notification or set action failures.
SampleMinimum
Minimum sampling interval.
Maximum number of sampled instances.
SampleInstance
Number of current sampled instances.
SampleInstancesHigh
SampleInstanceLacks
Number of sampling failures after the maximum number of sampled instances is reached.
display snmp mib event trigger
Use display snmp mib event trigger to display information about a trigger and the trigger tests.
display snmp mib event trigger [ owner trigger-owner name trigger-name ]
context-admin
context-operator
owner trigger-owner name trigger name: Specifies a trigger by its owner and name. The trigger-owner argument must be an existing SNMPv3 user. The trigger-name argument is case-sensitive string of 1 to 32 characters. If you do not specify a trigger, this command displays information about all triggers and trigger tests.
# Display information about the trigger identified by owner owner1 and name triggerA and the trigger tests.
<Sysname> display snmp mib event trigger owner owner1 name triggerA
  TriggerTest                 : existence | boolean | threshold
  TriggerObjOwner             : owner1
  TriggerObjName              : obj1
  Existence entry:
   ExiTest                    : present | absent
   ExiStartUp                 : present | absent
   ExiObjOwner                : owner1
   ExiObjName                 : object1
   ExiEvtOwner                : owner1
   ExiEvtName                 : event1
  Boolean entry:
   BoolCmp                    : unequal
   BoolValue                  : 1
   BoolStartUp                : true
   BoolEvtOwner               : N/A
   BoolEvtName                : N/A
  Threshold entry:
   ThresStartUp               : falling
   ThresRising                : 40
   ThresFalling               : 20
   ThresDeltaRising           : 40
   ThresDeltaFalling          : 20
   ThresObjOwner              : N/A
   ThresObjName               : N/A
   ThresRisEvtOwner           : owner1
   ThresRisEvtName            : event1
   ThresFalEvtOwner           : owner1
   ThresFalEvtName            : event1
   ThresDeltaRisEvtOwner      : owner1
   ThresDeltaRisEvtName       : event1
   ThresDeltaFalEvtOwner      : owner1
   ThresDeltaFalEvtName       : event1
Trigger entry
TriggerComment
Description for the trigger.
TriggerTest
Trigger test type:
·     Existence.
·     Boolean.
·     Threshold.
TriggerSampleType
Trigger sampling method:
·     absoluteValue—Absolute sampling.
·     deltaValue—Delta sampling.
TriggerValueID
OID of the monitored object.
Wildcarding option for the object OIDs:
·     false—Object OIDs are fully specified
·     true—Object OIDs are wildcarded.
TriggerTargetTag
Remote tag for the monitored object.
TriggerContextName
Context for an object.
Wildcarding option for the contexts
·     false—Contexts are fully specified.
·     true—Contexts are wildcarded.
TriggerFrequency
Trigger sampling interval.
TriggerObjOwner
Owner of the trigger object.
TriggerObjName
Name of the trigger object.
TriggerEnabled
Trigger status:
·     true—The trigger is enabled.
·     false—The trigger is disabled..
Existence entry
ExiTest
Type of the existence trigger test:
·     present.
·     absent.
·     changed.
ExiStartUp
Type of the existence trigger test for the first sampling:
·     present.
·     absent.
·     changed.
ExiObjOwner
Owner of the existence trigger test object.
ExiObjName
Name of the existence trigger test object.
ExiEvtOwner
Owner of the existence trigger test event.
ExiEvtName
Name of the existence trigger test event.
Boolean entry
BoolCmp
Boolean trigger test type:
·     unequal.
·     equal.
·     less.
·     lessOrEqual.
·     greater.
·     greaterOrEqual.
BoolValue
Reference value for the Boolean trigger test.
BoolStartUp
Whether the event is enabled for the first sampling:
·     true—The event is enabled for the first sampling.
·     false—The event is disabled for the first sampling.
BoolObjOwner
Owner of the Boolean trigger test object.
BoolObjName
Name of the Boolean trigger test object.
BoolEvtOwner
Owner of the Boolean event.
BoolEvtName
Name of the Boolean event.
Threshold entry
ThresStartUp
Threshold trigger test for the first sampling:
·     rising.
·     falling.
·     risingOrFalling.
ThresRising
Rising threshold.
ThresFalling
Falling threshold.
ThresDeltaRising
Delta rising threshold.
ThresDeltaFalling
Delta falling threshold.
ThresObjOwner
Owner of the threshold test object.
ThresObjName
Name of the threshold test object.
ThresRisEvtOwner
Owner of the rising event.
ThresRisEvtName
Name of the rising event.
ThresFalEvtOwner
Owner of the falling event.
ThresFalEvtName
Name of the falling event.
Owner of the Delta rising event.
Name of the Delta rising event.
Owner of the Delta falling event.
Name of the Delta falling event.
event (trigger-Boolean view)
Use event to specify an event for a Boolean trigger test.
Use undo event to restore the default.
undo event
No event is specified for a Boolean trigger test.
context-admin
owner event-owner: Specifies the owner of an event. Use the trigger owner as the event owner.
name event-name: Specifies the name of an event, a case-sensitive string of 1 to 32 characters.
# Specify an event for a Boolean trigger test.
[Sysname-trigger-owner1-triggerA-boolean] event owner owner1 name event1
test
event (trigger-existence view)
Use event to specify an event for an existence trigger test.
undo event
No event is specified for an existence trigger test.
Trigger-existence view
context-admin
# Specify an event for an existence trigger test.
[Sysname-trigger-owner1-triggerA] test existence
[Sysname-trigger-owner1-triggerA-existence] event owner owner1 name event1
test
event enable
Use event enable to enable an event.
Use undo event enable to disable an event.
event enable
undo event enable
An event is disabled.
Event view
context-admin
For an event to be triggered when the trigger condition is met, execute the event enable command.
# Enable the event identified by owner owner1 and name EventA.
[Sysname-event-owner1-EventA] event enable
action
snmp mib event
falling
Use falling to set a falling threshold and specify a falling event.
Use undo falling to restore the default.
undo falling { event | value }
The falling threshold is 0, and no falling event is specified.
context-admin
event owner event-owner: Specifies the owner of an event. Use the trigger owner as the event owner.
value integer-value: Specifies a falling threshold in the range of –2147483648 to 2147483647. The value must be smaller than or equal to the rising threshold.
A falling event is triggered if the value of the monitored object is smaller than or equal to the falling threshold.
If the value of the monitored object crosses the falling threshold at two or more samplings in succession, the event is triggered only at the first sampling.
# Set the falling threshold to 20.
[Sysname-trigger-owner1-triggerA-threshold] falling value 20
sample
test
frequency
Use frequency to set a sampling interval.
frequency interval
undo frequency
The sampling interval is 600 seconds.
Trigger view
context-admin
interval: Specifies a sampling interval in the range of 1 to 4294967295 seconds. The sampling interval must be greater than or equal to the minimum sampling interval.
To set the minimum sampling interval, execute the snmp mib event sample minimum command.
To avoid sampling failure, do not set the sampling interval too small when there are a large number of sampled objects.
# Set the sampling interval for a trigger to 360 seconds.
[Sysname-trigger-owner1-triggerA] frequency 360
object list (action-notification view)
Use object list to specify an object list for a notification action. The objects in the list will be added to the notification when the notification action is triggered.
Use undo object list to restore the default.
object list owner group-owner name group-name
undo object list
No object list is specified for a notification action.
Action-notification view
context-admin
owner group-owner: Specifies an object list owner. Use the event owner as the object list owner.
name group-name: Specifies an object list name, a case-sensitive string of 1 to 32 characters.
If you do not specify an object list for a notification action or the specified object list does not contain objects, no objects will be added to the triggered notification.
For more information, see "object list (trigger view)."
# Specify the object list identified by owner owner1 and name listA for the event identified by owner owner1 and name EventA.
[Sysname-event-owner1-EventA-notification] object list owner owner1 name listA
action
Use object list to specify an object list for a trigger. The objects in the list will be added to the triggered notification.
undo object list
No object list is specified for a trigger.
Trigger view
context-admin
owner group-owner: Specifies an object list owner. Use the trigger owner as the object list owner.
An object list is identified by its owner and name. After you specify a list of objects for a trigger, the objects in the list are added to the notification when the notification action is triggered.
You can configure the object list command in trigger view, trigger-test view (including trigger-Boolean view, trigger existence view, and trigger threshold view), and action-notification view. If the command is configured in any two of the views or all the three views, the object lists are added to the notification in the sequence: trigger view, trigger-test view, and action-notification view.
# Specify the object list identified by owner owner1 and name objectA for a trigger.
[Sysname-trigger-owner1-triggerA] object list owner owner1 name objectA
object list (trigger-Boolean view)
Use object list to specify an object list for a Boolean trigger test. The objects in the list will be added to the notification triggered by the test.
undo object list
No object list is specified for a Boolean trigger test.
context-admin
# Specify the object list identified by owner owner1 and name objectA for the trigger-Boolean trigger test.
[Sysname-trigger-owner1-triggerA-boolean] object list owner owner1 name objectA
test
object list (trigger-existence view)
Use object list to specify an object list for an existence trigger test. The objects in the list will be added to the notification triggered by the test.
undo object list
No object list is specified for an existence trigger test.
Trigger- existence view
context-admin
# Specify the object list identified by owner owner1 and name objectA for the existence trigger test.
[Sysname-trigger-owner1-triggerA-existence] object list owner owner1 name objectA
test
object list (trigger-threshold view)
Use object list to specify an object list for a trigger-threshold test. The objects in the list will be added to the notification triggered by the test.
undo object list
No object list is specified for a trigger-threshold test.
context-admin
# Specify the object list identified by owner owner1 and name objectA for the trigger-threshold test.
[Sysname-trigger-owner1-triggerA-threshold] object list owner owner1 name objectA
test
oid (action-notification view)
Use oid to specify a notification to be sent when the notification action is triggered.
Use undo oid to restore the default.
oid object-identifier
undo oid
The OID is 0.0. No notification is specified for a notification action.
context-admin
object-identifier: Specifies a notification by its OID, a case-sensitive string of 1 to 255 characters. It must be a trap node.
# Specify the notification identified by OID 1.3.6.1.2.1.14.16.2.1 for the event identified by owner owner1 and name EventA.
[Sysname-event-owner1-EventA-notification] oid 1.3.6.1.2.1.14.16.2.1
action
oid (action-set view)
Use oid to specify a set-action object.
undo oid
The OID is 0.0. No object is specified for a set action.
Action-set view
context-admin
object-identifier: Specifies an object by its OID or name, a case-sensitive string of 1 to 255 characters. The object can be a table node, conceptual row node, table column node, leaf node, or parent leaf node.
# Specify the object identified by OID 1.3.6.1.2.1.2.2.1.7.3 for the set action of an event identified by owner owner1 and name EventA.
[Sysname-event-owner1-EventA-set] oid 1.3.6.1.2.1.2.2.1.7.3
action
wildcard oid (action-set view)
oid (trigger view)
Use oid to specify a MIB object for trigger sampling.
undo oid
The OID is 0.0. No MIB object is specified for trigger sampling.
Trigger view
context-admin
# Specify the object identified by OID 1.3.6.1.2.1.2.2.1.1.3 for trigger sampling.
[Sysname-trigger-owner1-triggerA] oid 1.3.6.1.2.1.2.2.1.1.3
rising
Use rising to specify a rising threshold.
Use undo rising to restore the default.
undo rising { event | value }
The rising threshold is 0, and no rising event is specified.
context-admin
event owner event-owner: Specifies an event owner. Use the trigger owner as the event owner.
name event-name: Specifies an event name, a case-sensitive string of 1 to 32 characters.
value integer-value: Specifies a rising threshold in the range of –2147483648 to 2147483647. The value must be greater than or equal to the falling threshold.
If the value of the monitored object crosses the rising threshold at two or more samplings in succession, an event is triggered only at the first sampling.
# Set the rising threshold to 50 and specify the rising event identified by owner owner1 and name event1 for the threshold test.
[Sysname-trigger-owner1-triggerA-threshold] rising value 50
[Sysname-trigger-owner1-triggerA-threshold] rising event owner owner1 name event1
sample
test
sample
Use sample to specify a sampling method.
Use undo sample to restore the default.
sample { absolute | delta }
undo sample
The sampling method is absolute.
Trigger view
context-admin
absolute: Specifies the absolute sampling method. Use the current sampled value.
delta: Specifies the delta sampling method. Use the difference between the current sampled value and previous sampled value.
For delta sampling, obtain the difference between the current sampled value and previous sampled value as follows:
·     If the object value is UINT type, use the larger value to subtract the smaller value.
·     If the object value is INT type, use the present sampled value to subtract the previous sampled value.
# Specify the absolute sampling method.
[Sysname-trigger-owner1-triggerA] sample absolute
snmp mib event
Use snmp mib event to create an event and enter its view, or enter the view of an existing event.
Use undo snmp mib event to remove an event.
snmp mib event owner event-owner name event-name
undo snmp mib event owner event-owner name event-name
No event exists.
context-admin
event-owner: Specifies an event owner. The event owner must be an existing SNMPv3 user.
An event is identified by its owner and name.
# Create an event identified by owner owner1 and name EventA and enter its view.
action
description
event enable
snmp mib event
Use snmp mib event object list to configure an Event MIB object list.
Use undo snmp mib event object list to restore the default.
snmp mib event object list owner group-owner name group-name object-index oid object-identifier [ wildcard ]
undo snmp mib event object list owner group-owner name group-name object--index
No Event MIB object list is configured.
context-admin
owner group-owner: Specifies an object list owner. The object list owner must be an existing SNMPv3 user.
object-index argument: Specifies an object list index in the range of 1 to 4294967295.
oid object-identifier: Specifies an object by its OID or name, a case-sensitive string of 1 to 255 characters. The object can be a table node, a conceptual row node, a table column node, a leaf mode, or a parent leaf node.
wildcard: Enables wildcard search for objects. If you do not specify this keyword, the object is specified.
An object list is identified by its owner, name, and index. The specified objects in the object list will be carried in the triggered notification to the NMS.
# Configure an object list identified by owner owner1, name objectA, and index 10. Specify the object identified by OID 1.3.6.1.2.1.2.2.1.1.3 to be carried in the triggered notification.
[Sysname] snmp mib event object list owner owner1 name objectA 10 oid 1.3.6.1.2.1.2.2.1.1.3
snmp mib event
snmp mib event sample instance maximum
Use snmp mib event sample instance maximum to specify the maximum number of object instances that can be concurrently sampled.
Use undo snmp mib event sample instance maximum to restore the default.
snmp mib event sample instance maximum max-number
The maximum number of object instances that can be concurrently sampled is limited by the available resources. The value is 0.
context-admin
max-number: Specifies the maximum number of object instances that can be concurrently sampled. The value is in the range of 0 to 4294967295.
If you use the wildcard option for an object, Event MIB also samples the wildcarded object instances. Include the wildcarded object instances when you calculate the number of the concurrently sampled instances.
Changing the maximum number of object instances that can be concurrently sampled does not affect the existing instances. If the maximum number of object instances that can be concurrently sampled is changed to a value smaller than the number of existing instances, the existing instances will continue to be sampled.
# Set the maximum number to 10 for the object instances that can be concurrently sampled.
[Sysname] snmp mib event sample instance maximum 10
Use snmp mib event sample minimum to specify the minimum sampling interval.
Use undo snmp mib event sample minimum to restore the default.
snmp mib event sample minimum min-number
The minimum sampling interval is 1 second.
context-admin
min-number: Specifies the minimum sampling interval in the range of 1 to 2147483647, in seconds.
After you configure the minimum sampling interval, make sure the trigger sampling interval is greater than or equal to the minimum sampling interval.
Changing the minimum sampling interval does not affect the existing instances. If the minimum sampling interval is changed to a value smaller than the sampling interval of a trigger, the existing instances of the trigger will continue to be sampled at its interval.
# Set the minimum sampling interval to 50 seconds.
[Sysname] snmp mib event sample minimum 50
frequency
Use snmp mib event trigger to create a trigger and enter its view, or enter the view of an existing trigger.
Use undo snmp mib event trigger to remove a trigger.
snmp mib event trigger owner trigger-owner name trigger-name
undo snmp mib event trigger owner trigger-owner name trigger-name
No trigger exists.
context-admin
trigger-owner: Specifies a trigger owner, which must be an existing SNMPv3 user.
trigger-name: Specifies a trigger name, a case-sensitive string of 1 to 32 characters.
A trigger is identified by its owner and name. In trigger view, you can specify a monitored object and set an interval for sampling the object. An event is triggered when the sampled object meets the trigger condition.
If the trigger owner has no read access to the monitored object configured in trigger view, sampling on the object cannot be performed. For more information about SNMPv3 user access rights, see Network Management and Monitoring Configuration Guide.
# Create a trigger identified by owner owner1 and name triggerA.
snmp-agent trap enable event-mib
Use snmp-agent trap enable event-mib to enable the Event MIB trap feature.
Use undo snmp-agent trap enable event-mib to disable the Event MIB trap feature.
The Event MIB trap feature is enabled.
context-admin
After you enable the Event MIB trap feature, traps are generated when object sampling fails or a trigger condition is met and sent to the SNMP module. Traps include trigger trap, rising threshold break trap, falling threshold break trap, trigger-condition detection failure trap, and set-action trigger failure trap.
For the traps to be sent correctly, you must also configure SNMP on the device. For more information about SNMP configuration, see Network Management and Monitoring Configuration Guide.
# Enable the event MIB trap feature.
[Sysname] snmp-agent trap enable event-mib
startup (trigger-existence view)
Use startup to specify existence trigger test types for the first sampling.
Use undo startup to remove the existence trigger test types for the first sampling.
startup { absent | present }
undo startup { absent | present }
The existence trigger test types for the first sampling are present and absent.
context-admin
absent: Monitors the absence of a MIB object.
present: Monitors the presence of a MIB object.
For the first sampling, an event is triggered when the following conditions are met:
·     Both the startup and type commands specify the existence test type as present and the state of the monitored object changes to present at the first sampling. If the monitored objects are wildcarded, the event is triggered independently for each wildcarded object.
·     Both the startup command and type commands specify the existence trigger test type as absent and the state of the monitored object changes to absent at the first sampling. If the monitored objects are wildcarded, no event is triggered.
# Remove the present test configuration for the first sampling.
[Sysname-trigger-owner1-triggerA-existence] undo startup present
type
startup (trigger-threshold view)
Use startup to specify a threshold trap type for the first sampling.
Use undo startup to restore the default.
startup { falling | rising | rising-or-falling }
undo startup
The threshold trap type for the first sampling is rising-or-falling.
context-admin
falling: Specifies the falling trap.
rising: Specifies the rising trap.
rising-or-falling: Specifies the rising or falling trap.
If the trap type for the first sampling is rising or rising-or-falling, a rising trap is triggered when the first sample value is greater than or equal to the rising threshold.
If the trap type for the first sampling is rising or rising-or-falling, a falling trap is triggered when the first sample value is smaller than or equal to the rising threshold.
If the first sampling fails or the monitored object does not exist at the first sampling, the second sampling is considered the first sampling.
# Specify the rising trap for the first sampling.
[Sysname-trigger-owner1-triggerA-threshold] startup rising
sample
test
startup enable
Use startup enable to enable an event to be triggered for the first Boolean sampling.
Use undo startup enable to disable an event to be triggered for the first Boolean sampling.
startup enable
undo startup enable
An event is triggered for the first Boolean sampling.
context-admin
For an event to be triggered when a trigger condition is met at the first Boolean sampling, execute the startup enable command.
# Trigger an event for the first Boolean sampling.
[Sysname-trigger-owner1-triggerA-boolean] startup enable
comparison
value
test
Use test to specify a trigger test type and enter its view.
Use undo test to remove a trigger test type.
test { boolean | existence | threshold }
undo test { boolean | existence | threshold }
No test type is specified for a trigger.
Trigger view
context-admin
boolean: Specifies a Boolean trigger test. This test compares the value of the monitored object with the reference value.
existence: Specifies an existence trigger test. This test monitors the absence, presence, and change of the monitored object.
threshold: Specifies a threshold test. This test compares the value of the monitored object with the specified thresholds, such as rising threshold and falling threshold.
For more information about the trigger tests, see the commands in the trigger-Boolean view, trigger-existence view, and trigger-threshold view .
# Specify the existence test for a trigger.
trigger enable
Use trigger enable to enable a trigger.
Use undo trigger enable to disable a trigger.
trigger enable
undo trigger enable
A trigger is disabled.
Trigger view
context-admin
Before you enable a trigger, make sure the trigger meets the following conditions:
·     A monitored object is specified for the trigger.
·     The trigger sampling interval is greater than or equal to the minimum sampling interval.
# Create and enable a trigger.
[Sysname-trigger-owner1-triggerA] trigger enable
type
Use type to specify existence trigger test types.
Use undo type to remove the existence trigger test types.
type { absent | changed | present }
undo type { absent | changed | present }
The existence trigger test types are present and absent.
context-admin
absent: Monitors the absence of an object.
changed: Monitors the change of the value of an object. If the last sampling does not obtain a value, the event is not triggered.
present: Monitors the presence of an object.
For the first sampling, see "startup (trigger-existence view)".
The existence trigger tests also apply to the wildcarded instances of the monitor object.
# Specify the existence trigger test type as present.
[Sysname-trigger-owner1-triggerA-existence] type present
startup
test
value (action-set view)
Use value to set a value for a set-action object.
Use undo value to restore the default.
value integer-value
undo value
The value of a set-action object is 0.
Action-set view
context-admin
integer-value: Specifies a value for a set-action object. The value is in the range of –2147483648 to +2147483647.
# Set the value to 2 for the set-action object identified by OID 1.3.6.1.2.1.2.2.1.7.3.
action
mib event owner
oid
value (trigger-Boolean view)
Use value to set a reference value for a Boolean trigger test.
value integer-value
undo value
The reference value is 0.
context-admin
integer-value: Specifies a reference value in the range of –2147483648 to +2147483647.
A Boolean trigger test compares the sampled value with the reference value.
# Set the reference value to 5 for the Boolean trigger test.
[Sysname-trigger-owner1-triggerA-boolean] value 5
startup
test
wildcard context (action-set view)
Use wildcard context to enable wildcard search for the contexts of a set-action object.
Use undo wildcard context to restore the default.
wildcard context
The context of a set-action object is fully specified.
Action-set view
context-admin
This command must be used with the context command. A wildcarded context has two parts: the context specified by the context command and the wildcarded part.
# Specify the context for the set-action object as contextname1 and enable wildcard search for the contexts.
[Sysname-event-owner1-EventA-set] wildcard context
action set
context
wildcard context (trigger view)
Use wildcard context to enable wildcard search for the contexts of a monitored object.
wildcard context
The context of a monitored object is fully specified.
Trigger view
context-admin
# Specify the contexts for the monitored object as contextname and enable wildcard search for the contexts.
[Sysname-trigger-owner1-triggerA] wildcard context
context
Use wildcard oid to enable wildcard search for the set-action object OIDs.
Use undo wildcard oid to restore the default.
wildcard oid
undo wildcard oid
The set-action object OID is fully specified.
Action-set view
context-admin
This command must be used in conjunction with the oid command. A wildcarded OID has two parts: the OID specified by the oid command and the wildcarded part.
# Specify the set-action object by its OID 1.3.6.1.2.1.2.2.1.7 for the event identified by owner owner1 and name EventA. Enable wildcard search for the sec-action object OIDs.
[Sysname-event-owner1-EventA-set] wildcard oid
action set
oid
wildcard oid (trigger view)
Use wildcard oid to enable wildcard search for the monitored object OIDs.
wildcard oid
undo wildcard oid
A monitored object OID is fully specified.
Trigger view
context-admin
For example, to specify interface description nodes of all interfaces, execute the oid ifDescr and wildcard oid commands.
# Specify the sampled object by its OID 1.3.6.1.2.1.1.6 for a trigger and enable wildcard search for the monitored object OIDs.
[Sysname-trigger-owner1-triggerA] oid 1.3.6.1.2.1.1.6
[Sysname-trigger-owner1-triggerA] wildcard oid
oid