14-Common Industrial Protocols Configuration Guide

HomeSupportConfigure & DeployConfiguration GuidesH3C IE4300[IE4300-M][IE4320] Switch Series Configuration Guides-R63xx-6W10214-Common Industrial Protocols Configuration Guide
01-EtherNet IP configuration
Title Size Download
01-EtherNet IP configuration 421.43 KB

Contents

Configuring EtherNet/IP·· 2

About EtherNet/IP· 2

Benefits· 2

Network model 2

Communication mechanism·· 3

Restrictions: Software version compatibility with EtherNet/IP· 6

Restrictions and guidelines· 6

Enabling EtherNet/IP· 6

Display and maintenance commands for EtherNet/IP· 7

Appendix A  H3C device-specific object specifications· 7

Identity object (Class ID: 0x01) 7

Service codes· 7

Class attributes (instance=0) 8

Instance attributes (instance>0) 8

Message router object (Class ID: 0x02) 9

Service codes· 10

Class attributes (instance=0) 10

Instance attributes (instance>0) 10

Assembly object (Class ID: 0x04) 10

Service codes· 10

Class attributes (instance=0) 11

Instance attributes (instance>0) 11

Connection manager object (Class ID: 0x06) 11

Service codes· 11

Class attributes (instance=0) 12

Instance attributes (instance>0) 12

TCP/IP interface object (Class Code: 0xF5) 12

Service codes· 12

Class attributes (instance=0) 13

Instance attributes (instance>0) 13

Ethernet link object (Class Code: 0xF6) 15

Service codes· 15

Class attributes (instance=0) 15

Instance attributes (instance>0) 15

Appendix B  H3C device-specific CIP data in explicit messaging· 16

Requesting port and alarm data· 16

Port information· 17

Alarm information· 18

Requesting device status data· 18

Device information (01) 20

Port information (02) 21

RSTP information (03) 22

ERPS ring network information (04) 23

ERPS instance information (05) 24

RRPP domain information (06) 26

RRPP ring information (07) 26

Setting the device status· 28

Appendix C  H3C device-specific CIP data in implicit messaging· 29

Output message· 29

Input message· 30

Port information in the input message· 30

Alarm information in the input message· 32

 


Configuring EtherNet/IP

About EtherNet/IP

Ethernet/Industrial Protocol (EtherNet/IP) is an industrial network control technology defined and maintained by the Open DeviceNet Vendor Association (ODVA). Built on standard Ethernet and TCP/IP technologies, EtherNet/IP uses Ethernet protocols at the physical and data link layers, TCP/IP protocol family at the network and transport layers, and Common Industrial Protocol (CIP) at the application layer. EtherNet/IP can meet the real-time and reliable communication requirements in high-load industrial networks, and it is widely used in industrial Ethernet networks.

Benefits

EtherNet/IP has the following technical benefits:

·     Open: EtherNet/IP uses the TCP/IP protocol stack. It can use existing standard Ethernet hardware and be compatible with existing industrial Ethernet networks.

·     Standardized: EtherNet/IP contains recognized standards defined by ODVA. It provides a unified communication standard for different industrial devices and systems and allows smooth communication between devices from different vendors.

·     Safe and reliable: The application layer CIP protocol of EtherNet/IP has a built-in mechanism for secure and reliable data transmission.

·     Scalable: The application layer CIP protocol of EtherNet/IP is an expandable protocol that can be extended and customized based on different application scenarios and requirements.

Network model

As shown in Table 1, EtherNet/IP uses the same physical layer, data link layer, and transport layer as standard Ethernet and adds an encapsulation layer above the transport layer. This encapsulation layer is used to package the CIP data coming from the application layer into a standard format.

Figure 1 EtherNet/IP network model

 

Communication mechanism

Messaging type

EtherNet/IP uses two types of messaging for communication between devices: explicit messaging and implicit messaging.

·     Explicit messaging: Data is transmitted through TCP, suitable for scenarios that require accurate message delivery and are not time critical, such as configuring device information and uploading or downloading programs.

·     Implicit messaging: Data is transmitted through UDP, suitable for transmission of time-critical data such as I/O data. A CIP connection must be established before implicit messaging. CIP connection is a CIP protocol service. After the connection is established, the two ends each hold a connection ID for subsequent information exchange.

Communication model

Explicit communication

EtherNet/IP explicit communication uses a client/server model in which the industrial control device (controller) acts as the client, and peripheral I/O sensors, valves, industrial switches, or other measuring devices (devices) act as servers. The communication is initiated by the client, which sends a request to the servers. The servers respond accordingly after receiving the request.

Figure 2 EtherNet/IP explicit communication model

 

Implicit communication

EtherNet/IP implicit communication uses a producer/consumer model. In this model, the devices act as data producers. They send their data onto the network all at once, allowing the controller to selectively read the data they require. This greatly enhances the communication efficiency of the entire EtherNet/IP network system.

Figure 3 EtherNet/IP implicit communication model

 

Message formats

Explicit communication message format

In explicit communication mode, EtherNet/IP encapsulates the CIP protocol data in the following format.

Figure 4 Explicit communication message format

 

The EtherNet/IP explicit encapsulation package includes an encapsulation header and encapsulation data. The encapsulation header contains the following fields:

·     Command: EtherNet/IP command that describes the function and purpose of the message, in 2 bytes.

·     Length: Length of the data following the encapsulation header, in 2 bytes.

·     Session Handle: TCP session handle, in 4 bytes.

·     Status: Execution status of the EtherNet/IP command, in 4 bytes.

·     Sender Context: Description of sender information, in 8 bytes.

·     Options: Optional field, a maximum of 4 bytes.

The encapsulating data contains the following fields:

·     Item Count: Total number of items in the packaged data.

·     Address Item: Destination address information, including the address type, address length, and specific address.

·     Data Item: CIP protocol data information, including the data type, data length, and specific data. The specific data includes the CIP command and request path.

Implicit communication message format

In implicit communication mode, EtherNet/IP encapsulates the CIP protocol data in the following format.

Figure 5 Implicit communication message format

 

The EtherNet/IP explicit encapsulation package includes only the encapsulation data, which contains the following fields:

·     Item Count: Total number of items in the packaged data.

·     Address Item: Destination address information, including the address type, address length, CIP connection ID, and specific address. In implicit communication mode, EtherNet/IP determines the target by the connection ID.

·     Data Item: CIP protocol data information, including the data type, data length, and specific data. The specific data includes the CIP command and request path.

CIP object model

Each CIP node is a set of objects, and the targets of CIP communication are these specific objects. For EtherNet/IP communication, you can define specific components on a device as different objects.

Objects use a three-dimensional structure with classes, instances, and attributes. Multiple classes can exist on a CIP node, each class can have multiple instances, and each instance can have multiple attributes, as shown in Figure 6.

Figure 6 CIP object model diagram

 

Restrictions: Software version compatibility with EtherNet/IP

EtherNet/IP is supported only in F6355P05 and later.

Restrictions and guidelines

H3C industrial switches can act only as devices in EtherNet/IP communication. The term "device" in this configuration procedure collectively refers to H3C industrial switches.

Enabling EtherNet/IP

About this task

After EtherNet/IP is enabled on a device, the device can establish a TCP or UDP connection with the controller and perform EtherNet/IP communication over this connection. The controller can read and write the data or status of the device over EtherNet/IP. The device uses port number 44818 for establishing TCP connections and port number 2222 for establishing UDP connections.

Arbitrarily changing the status of the device might pose serious security risks to the entire network when a misoperation or malicious attack is present in the network. In such scenarios, switch the EtherNet/IP operating mode on the device to read-only mode. This ensures that the controller can only read information from the device via EtherNet/IP.

Prerequisites

The device uses VLAN 1 as the EtherNet/IP management VLAN for communication with the controller. Before enabling EtherNet/IP, first assign an IP address to VLAN interface 1.

Restrictions and guidelines

The controller can differentiate data of ports in the total data sent by the lower-level device by the port ID displayed in the display ethernet-ip information command.

Currently, the controller can read and modify the information of 128 ports on a device simultaneously.

Some CIP commands require a specific transport layer connection for EtherNet/IP communication.

Table 1 CIP command codes and required transport layer connection

Command code

Name

Connection method

0x0000

NOP

TCP

0x0004

ListServices

TCP or UDP

0x0063

ListIdentity

TCP or UDP

0x0064

ListInterfaces

TCP or UDP

0x0065

RegisterSession

TCP

0x0066

UnRegisterSession

TCP

0x006F

SendRRData

TCP

0x0070

SendUnitData

TCP

0x0072

IndicateStatus

TCP

0x0073

Cancel

TCP

 

Procedure

1.     Enter system view.

system-view

2.     Enable EtherNet/IP.

ethernet-ip enable

By default, EtherNet/IP is disabled.

3.     (Optional) Set the EtherNet/IP operating mode to read-only.

ethernet-ip working-mode read-only

By default, the EtherNet/IP operating mode is read/write. In read/write mode, the device allows read/write operations from the controller over EtherNet/IP.

Display and maintenance commands for EtherNet/IP

Execute display commands in any view.

 

Task

Command

Display information required for reading port information via EtherNet/IP.

display ethernet-ip information interface { interface-type interface-number | interface-name }

 

Appendix A  H3C device-specific object specifications

"instance=0" indicates a class attribute, which is shared by all objects within the same class. "instance>0" indicates an instance attribute, which is unique to an object instance.

Identity object (Class ID: 0x01)

Service codes

Service code

Need in implementation

Service name

Description

instance=0

instance>0

0x0E

Conditional (√)

Conditional (√)

Get_Attribute_Single

Reads the specified attribute.

0x05

Optional (x)

Required (√)

Reset

Invokes the reset service for the device.

0x01

Optional (√)

Conditional (√)

Get_Attributes_All

Reads multiple attributes of the object.

 

Class attributes (instance=0)

Class attribute

Need in implementation

Access rule

Attribute name

Data type

Description

0x01

Get

Revision

USHORT

Object revision.

0x02

Get

Number of instances

USHORT

Number of object instances currently created in this class level of the device.

0x06

Get

Number of max attributes

USHORT

Maximum number of attributes in the current class.

0x07

Get

Number of max instance attributes

USHORT

Maximum number of attributes in the current instance.

 

Instance attributes (instance>0)

Instance attribute

Need in implementation

Access rule

Name

Data type

Description

0x01

Get

Vendor ID

UINT

Vendor ID.

0x02

Get

Device type

UINT

Device type.

0x03

Get

Product code

UINT

Product code:

·     2465: H3C IE4320-28S

·     2463: H3C IE4320-28P

·     2464: H3C IE4320-28S-HPWR

·     2479: H3C IE4320-52S

·     2478: H3C IE4320-52P

·     2487: H3C IE4320-28S-PS1

·     2552: H3C IE4320-12P-UPWR

·     2551: H3C IE4320-28F

·     2579: H3C IE4320-6P

·     2576: H3C IE4320-12P

·     2578: H3C IE4320-20P

·     2577: H3C IE4320-6P-AC

·     2604: H3C IE4320-12P-PWRM

·     3470: H3C IE4320-28P-K

·     3469: H3C IE4320-28P-S

·     1749: H3C IE4300-28P-M

·     1974: H3C IE4300-12P-PWR-M

·     2225: H3C IE4300-12P-AC

·     2226: H3C IE4300-12P-PWR

·     25506: H3C Simware32/H3C Simware64

0x04

Get

Revision

STRUCT

Device revision, including major and minor revisions, displayed in the major.minor format.

Major revision

USINT

Major revision range: 0x 01 to 0x 7F.

Minor revision

USINT

Minor revision range: 0x01 to 0xFF.

0x05

Get

Status

WORD

Device status.

0x06

Get

Serial number

UDINT

Serial number.

0x07

Get

Product name

STRING

Product name.

 

Message router object (Class ID: 0x02)

The message router object strips the header of messages received from the Unconnected Message Manager (UCMM) or Transport, and parses the data. Then, it routes the service to the target class or attribute.

Service codes

Service code

Need in implementation

Service name

Description

Class attribute

Instance attribute

0x0E

Required (√)

Required (√)

Get_Attribute_Single

Reads the specified attribute.

0x01

Conditional (√)

Conditional(√)

Get_Attribute_All

Reads the value of multiple attributes of the object.

 

Class attributes (instance=0)

Class attribute

Need in implementation

Access rule

Name

Data type

Description

0x01

Get

Revision

UINT

Object revision

0x02

Get

Max instance

UINT

Maximum instance number of an object currently created in this class level of the device.

0x03

Get

Number of instances

UINT

Number of object instances currently created at this class level of the device.

 

Instance attributes (instance>0)

No instance attributes are currently available for the message router object.

Assembly object (Class ID: 0x04)

The assembly object binds attributes of multiple objects. It defines the parameters for I/O data exchange.

Service codes

Service code

Need in implementation

Service name

Description

Static assembly

Dynamic assembly (unsupported currently)

 

Class attribute

Instance attribute

Class attribute

Instance attribute

 

 

0x0E

Conditional (√)

Required (√)

Required (√)

Required (√)

Get_Attribute_Single

Reads the specified attribute.

0x08

N/A

N/A

Required

N/A

Create

 

0x10

N/A

Optional (√)

N/A

Conditional (√)

Set_Attribute_Single

Sets the specified attribute.

0x09

N/A

N/A

Conditional

Required

Delete

Deletes the assembly object and releases the resources.

 

Class attributes (instance=0)

Class attribute

Need in implementation

Access rule

Name

Data type

Description

0x01

Get

Revision

UINT

Object revision

0x02

Get

Max instance

UINT

Maximum instance number of an object currently created in this class level of the device.

0x03

Get

Number of instances

UINT

Number of object instances currently created at this class level of the device.

 

Instance attributes (instance>0)

Instance attribute

Need in implementation

Access rule

Name

Data type

Description

0x03

Required (√)

Get/Set

Data

ARRAY of BYTE

I/O connection data.

 

Connection manager object (Class ID: 0x06)

The connection manager object is responsible for establishment and termination of Common Industrial Protocol (CIP) connections.

Service codes

Service code

Need in implementation

Service name

Description

Class attribute

Instance attribute

0x01

Optional (√)

Optional (√)

Get_Attributes_All

Reads multiple attributes of the object.

0x0E

Conditional (√)

Conditional (√)

Get_Attribute_Single

Reads the specified attribute.

0x4E

N/A

Conditional (√)

Forward_Close

Closes a CIP connection.

0x54

N/A

Conditional (√)

Forward_Open

Opens a CIP connection.

0x5A

N/A

Conditional (√)

Get_Connection_Owner

Determines the owner of a redundant connection.

 

Class attributes (instance=0)

Class

Attribute

Need in implementation

Access rule

Name

Data type

Description

0x01

Get

Revision

UINT

Object revision

0x02

Get

Max instance

UINT

Maximum instance number of an object currently created in this class level of the device.

0x03

Get

Number of instances

UINT

Number of object instances currently created at this class level of the device.

 

Instance attributes (instance>0)

No instance attributes are available currently for the connection manager object.

TCP/IP interface object (Class Code: 0xF5)

The TCP/IP interface object provides the mechanism to configure TCP/IP network interfaces on a device.

Service codes

Service code

Need in implementation

Service name

Description

Class attribute

Instance attribute

0x01

Optional (√)

Optional (√)

Get_Attributes_All

Reads multiple attributes of the object.

0x0E

Conditional (√)

Required (√)

Get_Attribute_Single

Reads the specified attribute.

0x10

N/A

Required (√)

Set_Attribute_Single

Sets the specified attribute.

 

Class attributes (instance=0)

Class

Attribute

Need in implementation

Access rule

Attribute name

Data type

Description

0x01

Get

Revision

UINT

Object revision

0x02

Get

Max instance

UINT

Maximum instance number of an object currently created in this class level of the device.

0x03

Get

Number of instances

UINT

Number of object instances currently created at this class level of the device.

 

Instance attributes (instance>0)

Class attribute

Need in implementation

Access rule

Attribute name

Data type

Description

Remarks

0x01

Get

Status

DWORD

IP configuration status

·     0—Not configured.

·     1—Valid configuration obtained from Bootstrap Protocol (BOOTP), Dynamic Host Configuration Protocol (DHCP), or non-volatile storage.

·     2—Configured by hardware.

0x02

Get

Configuration capability

DWORD

Configuration capability supported by the device

·     0—BOOTP client

·     1—DNS client

·     2—DHCP client

·     3—DHCP-DNS update

·     4—Configuration settable

·     5 to 31—Reserved

0x03

Get/Set

Configuration

control

DWORD

Interface IP mode

 

0x04

Get

Physical link object

STRUCT

of:

Path of the physical link object

The obtained attribute is a structure composed of the following members.

Path size

UINT

Path size

 

Path

EPATH

Specific path information

 

0x05

Get/Set

Interface configuration

STRUCT

of:

TCP/IP network configuration information of the device

The obtained attribute is a structure composed of the following members.

IP address

UDINT

IP address of the device

 

Network mask

UDINT

Subnet mask of the device

 

Gateway address

UDINT

Gateway of the device

 

Name server

UDINT

Primary name server

 

Name server 2

UDINT

Secondary name server

 

Domain name

STRING

Default domain name

 

0x06

Get/Set

Host name

STRING

Device name

 

0x08

Get

Set is conditional

TTL value

USINT

TTL value of EtherNet/IP multicast packets

 

0x09

Get

Set is conditional

Mcast config

STRUCT of:

Multicast IP address configuration information

The obtained attribute is a structure composed of the following members.

Alloc control

USINT

Multicast address allocation status

 

Reserved

USINT

 

 

Num Mcast

UINT

Number of allocable multicast addresses

 

 

Ethernet link object (Class Code: 0xF6)

An Ethernet link maintains link-specific counters and status information for an Ethernet interface.

Service codes

Service code

Need in implementation

Service name

Description

Class attribute

Instance attribute

0x01

Optional (√)

Optional (√)

Get_Attributes_All

Reads multiple attributes of the object.

0x0E

Conditional (√)

Required (√)

Get_Attribute_Single

Reads the specified attribute.

 

Class attributes (instance=0)

Class

Attribute

Need in implementation

Access rule

Attribute name

Data type

Description

0x01

Get

Revision

UINT

Object revision

0x02

Get

Max instance

UINT

Maximum instance number of an object currently created in this class level of the device.

0x03

Get

Number of Instances

UINT

Number of object instances currently created at this class level of the device.

 

Instance attributes (instance>0)

Class attribute

Need in implementation

Access rule

Attribute name

Data type

Description

Remarks

0x01

Get

Interface speed

DWORD

Interface speed

10 Mbps

100 Mbps

1 G

0x02

Get

Interface flags

DWORD

Interface flags

 

0x03

Get

Physical address

ARRAY of 6 USINTS

MAC address

 

0x0A

Get

Interface label

SHORT_

STRING

Interface name

 

 

Appendix B  H3C device-specific CIP data in explicit messaging

To retrieve or set the status of an H3C device, the industrial control device (controller) must first send a request carrying the set attribute single command to that device. Subsequently, the controller sends a request carrying the get attribute single command to formally request the data.

 

Service

Parameters

set attribute single

Service: 16

Class: 4

Instance: 104

Attribute: 3

Get attribute single

Service: 14

Class: 4

Instance: 103

Attribute: 3

 

Requesting port and alarm data

To retrieve port and alarm data of an H3C device, the controller needs to send a request that carries the set attribute single command to that device. This request populates the first two bytes of the data portion with 0x0000, and the succeeding bytes as follows:

 

Third byte

Fourth byte

00

01

02

03

04

05

n

Port status and alarms (00)

 

 

 

 

 

 

 

 

 

After receiving the request packet with the get attribute single command, the H3C device replies to the controller with a response packet. The value starting at position 05 in the response message is as follows:

Port information

Input byte offset num

Status item

Position in the data portion of the packet (byte)

Each byte represents the status of four ports. The port status occupies 32 bytes. The succeeding bytes are alarm information.

0

Status of ports 1 to 4

1

Status of ports 5 to 8

2

Status of ports 9 to 12

3

Status of ports 13 to 16

4

Status of ports 17 to 20

5

Status of ports 21 to 24

6

Status of ports 25 to 28

7

Status of ports 29 to 32

8

Status of ports 33 to 36

9

Status of ports 37 to 40

10

Status of ports 41 to 44

11

Status of ports 45 to 48

12

Status of ports 49 to 52

13

Status of ports 53 to 56

14

Status of ports 57 to 60

15

Status of ports 61 to 64

16

Status of ports 65 to 68

17

Status of ports 69 to 72

18

Status of ports 73 to 76

19

Status of ports 77 to 80

20

Status of ports 81 to 84

21

Status of ports 85 to 88

22

Status of ports 89 to 92

23

Status of ports 93 to 96

24

Status of ports 97 to 100

25

Status of ports 101 to 104

26

Status of ports 105 to 108

27

Status of ports 109 to 112

28

Status of ports 113 to 116

29

Status of ports 117 to 120

30

Status of ports 121 to 124

31

Status of ports 125 to 128

The status of each port is represented by 2 bits. The available port status in binary are:

·     00: Disabled

·     01: Up

·     10: Down

A port is considered enabled if it is in up or down state.

 

Alarm information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

32

Port 1 alarm status

0x00: disable

0x01: normal

0x02: alarm

1

33

Port 2 alarm status

0x00: disable

0x01: normal

0x02: alarm

1

34

Ports 3 to 128 alarm status

Each port occupies 1 byte

0x01: normal

0x02: alarm

62

160

Temperature alarm status

0x01: normal

0x02: alarm

1

161

CPU alarm status

0x01: normal

0x02: alarm

1

162

Memory alarm status

0x01: normal

0x02: alarm

1

163

Power supply alarm status

0x01: normal

0x02: Power supply 1 alarm

0x03: Power supply 2 alarm

1

164 to 255

Reserved

 

 

 

Requesting device status data

To retrieve status data of an H3C device, the controller sends a request that carries the set attribute single command to that device. This request populates the first two bytes of the data portion with 0x0000, and the succeeding bytes as follows:

 

Third byte

Fourth byte

Fifth byte

Data category (Table)

Data category (node)/index

Data subcategory (node)/subindex

00

01

02

03

04

05

06

n(ff)

00

01

...

n

01 (Device information)

 

Vendor name

Device type

Vendor address

Phone number

Product name

Additional information

 

 

\

02 (Port information)

 

First port

Second port

Third port

Fourth port

Fifth port

Sixth port

 

Nth port

\

03 (RSTP information)

Global info

Ring network info on the first port

Ring network info on the second port

Ring network info on the third port

Ring network info on the fourth port

Ring network info on the fifth port

Ring network info on the sixth port

 

Ring network info on the Nth port

\

04 (ERPS ring network info)

Global info

First ERPS ring info

Second ERPS ring info

Third ERPS ring info

Fourth ERPS ring info

Fifth ERPS ring info

Sixth ERPS ring info

 

Nth ERPS ring info

\

05 (ERPS ring instance info)

Global info

First ERPS ring info

Second ERPS ring info

Third ERPS ring info

Fourth ERPS ring info

Fifth ERPS ring info

Sixth ERPS ring info

 

Nth ERPS ring info

\

First instance info

...

Nth instance info

06 (RRPP domain info)

Global info

First RRPP domain info

Second RRPP domain info

Third RRPP domain info

Fourth RRPP domain info

Fifth RRPP domain info

Sixth RRPP domain info

 

Nth RRPP domain info

\

07 (RRPP ring network info)

Global info

First RRPP domain info

Second RRPP domain info

Third RRPP domain info

Fourth RRPP domain info

Fifth RRPP domain info

Sixth RRPP domain info

 

Nth RRPP domain info

\

First RRPP ring information

...

Nth RRPP ring information

 

After receiving the request packet with the get attribute single command, the H3C device replies to the controller with a response packet. The value starting from position 05 in the response packet is as follows:

Device information (01)

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

Serial number

 

33

35

Boot ROM version

 

64

99

Current running software version

 

64

163

Device IP address

192.168.0.1

(C0 A8 00 01)

 

4

167

MAC address of the MPU

 

4

171

Device bridge MAC address

 

6

177

Power supply 1 status information

0x00: Power off

0x01: Power on

1

178

Power supply 2 status information

0x00: Power off

0x01: Power on

1

179

CPU usage in percentage (long term)

 

4

183

CPU usage in percentage (short term)

 

4

187

Total memory (bytes)

 

4

191

Free memory (bytes)

 

4

195

Device uptime (minutes)

 

8

203 to 255

Reserved

 

 

 

Port information (02)

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

Port name

 

64

66

Port state

·     0x00: Disabled

·     0x01: Up

·     0x02: Down

1

67

Port speed

 

1

68

Duplex mode

·     0x01: Half

·     0x02: Full

·     0x03: Auto

1

69

Flow control enabling status

·     0x00: Off

·     0x01: On

1

70

Received packet count

 

8

78

Received byte count

 

8

86

Transmitted packet count

 

8

94

Transmitted byte count

 

8

102

Received unicast packet count

 

8

110

Received multicast packet count

 

8

118

Received broadcast packet count

 

8

126

Transmitted unicast packet count

 

8

134

Transmitted multicast packet count

 

8

142

Transmitted broadcast packet count

 

8

150

Received pause frame count

 

8

158

Transmitted pause frame count

 

8

166

Received CRC error packet count

 

8

174 to 255

Reserved

 

 

 

RSTP information (03)

RSTP global information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

RSTP global enabling status

·     0—Disabled

·     1—Enabled

2

04

Root bridge ID

8 byes

8

12

Bridge ID

8 byes

8

20

Priority

Value range: 0 to 61440

4

24

Hello time at which the root device sends BPDUs

Value range: 1 to10

4

28

Max age of BPDUs

Value range: 6 to 40

4

32

Forward delay

Value range: 4 to 30

4

 

RSTP port information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

RSTP port enabling status

·     0—Disabled

·     1—Enabled

2

04

Port priority

Value range: 0 to 240

4

08

Path cost

Value range: 0 to 200000000

4

12

Port role

·     0—Disabled port

·     1—Alternate port

·     2—Backup port

·     3—Root port

·     4—Designated port

·     5—Master port

4

16

Port state

·     1—Discarding

·     2—Learning

·     3—Forwarding

4

 

ERPS ring network information (04)

ERPS ring network global information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

ERPS global enabling status

0: disable

1: enable

2

 

ERPS ring information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

ERPS ring ID

Value range: 1 to 8

2

04

ERPS ring member port 0

Port name

64

68

RPS ring member port 1

Port name

64

132

ERPS ring instance list

 

64

197-255

 

Reserved

 

 

 

 

ERPS instance information (05)

ERPS ring network global information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

ERPS global enabling status

0: disable

1: enable

2

 

ERPS instance information

Position in the data portion of the message

(byte)

Name

Value

Length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

ERPS ring ID

Value range: 1 to 8

2

04

ERPS instance ID

Value range: 1 to 64

2

06

ERPS instance enabling status

0: The instance is not enabled.

1: The instance is enabled.

1

07

Control VLAN of the ERPS instance

Value range: 2 to 4094

2

09

Node role

String.

·     Owner: Owner node.

·     Neighbor: Neighbor

·     Interconnection: Interconnection node

·     Normal: Normal node

32

41

Node state

String.

·     Idle: Stable state when all non-RPL links are available

·     Protection: State when a non-RPL link is faulty. In this state, the RPL link is unblocked to forward traffic. All nodes enter the protection state after a node enters the protection state.

·     MS: State when traffic paths are manually switched.

·     FS: State when traffic paths are forcibly switched.

·     Pending: Transitional state between two states.

·     -: ERPS is disabled globally or for the instance.

32

73

ERPS ring member port 0

Port name.

64

137

Role of ERPS ring member port 0

String.

·     RPL

·     Non-RPL

8

145

State of ERPS ring member port 0

String.

·     Blocked

·     Up

·     Down

8

153

ERPS ring member port 1

Port name.

64

217

Role of ERPS ring member port 1

Port role. String.

·     RPL

·     Non-RPL

8

225

State of ERPS ring member port 1

Port state. String.

·     Blocked

·     Up

·     Down

8

233-255

Reserved

 

 

 

RRPP domain information (06)

RRPP ring network global information

Data portion

position (byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

RRPP global enabling status

0: disable

1: enable

2

 

RRPP domain information

Data portion

position (byte)

Name

Value

Data length (bytes)

Position in the data portion of the message

(byte)

Data name

Data example

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

RRPP domain ID

Value range: 1 to 8

2

04

Control VLAN of the RRPP domain

Value range: 2 to 4094

2

06

Ring list of the RRPP domain

 

128

 

RRPP ring information (07)

RRPP ring network global information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

RRPP global enabling status

0: Disabled

1: Enabled

2

 

RRPP ring information

Position in the data portion of the message

(byte)

Name

Value

Data length (bytes)

00

Whether the request is successful or failed

0x0000: Successful.

0xFFFF: Failed

2

02

RRPP domain ID

Value range: 1 to 8

2

04

RRPP ring ID

Value range: 1 to 64

2

06

Ring level

·     0—Primary ring

·     1—subring

1

07

RRPP ring enabling status

·     0—RRPP ring is not enabled.

·     1— RRPP ring is enabled.

1

08

Node role

·     0—Transit node

·     1—Master node

·     2—Edge node

·     3—Assistant edge node

1

09

RRPP ring state

·     0—Completed

·     1—Failed

·     2—LinkUp

·     3—LinkDown

·     4—PreForward

·     5—LinkUpNotify

·     6—LinkDnNotify

·     7—PreForwardNotify

·     8—Unknown

1

10

RRPP ring primary port

Value range: 1 to 128

4

14

RRPP ring primary port status

Port status:

·     0—down.

·     1—up.

·     2—blocked.

1

15

RRPP ring secondary port

Value range: 1 to 128

4

19

RRPP ring secondary port status

Port status:

·     0—down.

·     1—up.

·     2—blocked.

1

20

RRPP ring edge port

Value range: 1 to 128

4

24

RRPP ring edge port status

Port status:

·     0—down.

·     1—up.

·     2—blocked.

1

 

Setting the device status

To set the port status of an H3C device, the controller sends a request that carries the set attribute single command to the device. This request populates the first two bytes of the data portion with 0x0100, and the succeeding bytes as follows:

 

Input byte offset num

Status item

Position in the data portion of the message (byte)

 

3

Status for ports 1 to 4

4

Status of ports 5 to 8

5

Status of ports 9 to 12

6

Status of ports 13 to 16

7

Status of ports 17 to 20

8

Status of ports 21 to 24

9

Status of ports 25 to 28

10

Status of ports 29 to 32

11

Status of ports 33 to 36

12

Status of ports 37 to 40

13

Status of ports 41 to 44

14

Status of ports 45 to 48

15

Status of ports 49 to 52

16

Status of ports 53 to 56

17

Status of ports 57 to 60

18

Status of ports 61 to 64

19

Status of ports 65 to 68

20

Status of ports 69 to 72

21

Status of ports 73 to 76

22

Status of ports 77 to 80

23

Status of ports 81 to 84

24

Status of ports 85 to 88

25

Status of ports 89 to 92

26

Status of ports 93 to 96

27

Status of ports 97 to 100

28

Status of ports 101 to 104

29

Status of ports 105 to 108

30

Status of ports 109 to 112

31

Status of ports 113 to 116

32

Status of ports 117 to 120

33

Status of ports 121 to 124

34

Status of ports 125 to 128

The port status of each port is represented by 2 bits. The binary value 01 represents to enable the port, 10 represents to disable the port, and 00 and 11 represent to keep the port status unchanged.

 

Appendix C  H3C device-specific CIP data in implicit messaging

A CIP connection must be established between an H3C device and the controller to initiate implicit communication. The connection parameters need to be configured as follows:

 

Transport type

Class ID

Instance ID

Connection point

Data size

Input

4

3

101 0x65

200 bytes

Output

102 0x66

40 bytes

 

The output message in implicit communication contains the desired status for each port. The Input message contains the current status and alarm information of each port.

Output message

The output message describes the desired status for each port.

 

Input byte offset num

Status item

Position in the data portion of the message (byte)

Transaction number. The device will process the output message (2 bytes) only when the transaction number is updated. If the transaction number is not updated, the succeeding message portion will not be read and analyzed.

 

Run idle buf, which is set to 0 (4bytes). The output length set in the connection point starts counting from below. The data location is also counted from below.

0

Status of ports 1 to 4

1

Status of ports 5 to 8

2

Status of ports 9 to 12

3

Status of ports 13 to 16

4

Status of ports 17 to 20

5

Status of ports 21 to 24

6

Status of ports 25 to 28

7

Status of ports 29 to 32

8

Status of ports 33 to 36

9

Status of ports 37 to 40

10

Status of ports 41 to 44

11

Status of ports 45 to 48

12

Status of ports 49 to 52

13

Status of ports 53 to 56

14

Status of ports 57 to 60

15

Status of ports 61 to 64

16

Status of ports 65 to 68

17

Status of ports 69 to 72

18

Status of ports 73 to 76

19

Status of ports 77 to 80

20

Status of ports 81 to 84

21

Status of ports 85 to 88

22

Status of ports 89 to 92

23

Status of ports 93 to 96

24

Status of ports 97 to 100

25

Status of ports 101 to 104

26

Status of ports 105 to 108

27

Status of ports 109 to 112

28

Status of ports 113 to 116

29

Status of ports 117 to 120

30

Status of ports 121 to 124

31

Status of ports 125 to 128

32 to 39

Reserved

The first 32 bytes of the message indicate the desired status for the ports, with 2 bits for each port. 01 represents to enable the port, 10 represents to disable the port, 00 and 11 represent to keep the port status unchanged. The last eight bytes are reserved.

 

Input message

The input message describes the current status of ports.

Port information in the input message

Input byte offset num

Status item

Position in the data portion of the message (byte)

Transaction number. The device will process the output message (2 bytes) only when the transaction number is updated. If the transaction number is not updated, the succeeding message portion will not be read and analyzed. The output length set in the connection point starts counting from below. The data location is also counted from below.

0

Status of ports 1 to 4

1

Status of ports 5 to 8

2

Status of ports 9 to 12

3

Status of ports 13 to 16

4

Status of ports 17 to 20

5

Status of ports 21 to 24

6

Status of ports 25 to 28

7

Status of ports 29 to 32

8

Status of ports 33 to 36

9

Status of ports 37 to 40

10

Status of ports 41 to 44

11

Status of ports 45 to 48

12

Status of ports 49 to 52

13

Status of ports 53 to 56

14

Status of ports 57 to 60

15

Status of ports 61 to 64

16

Status of ports 65 to 68

17

Status of ports 69 to 72

18

Status of ports 73 to 76

19

Status of ports 77 to 80

20

Status of ports 81 to 84

21

Status of ports 85 to 88

22

Status of ports 89 to 92

23

Status of ports 93 to 96

24

Status of ports 97 to 100

25

Status of ports 101 to 104

26

Status of ports 105 to 108

27

Status of ports 109 to 112

28

Status of ports 113 to 116

29

Status of ports 117 to 120

30

Status of ports 121 to 124

31

Status of ports 125 to 128

The status of each port is represented by 2 bits:

·     00: Disabled

·     01: Up

·     10: Down

A port is considered enabled if it is in up or down state.

 

Alarm information in the input message

Position in the data portion of the message (byte)

Name

Value

Data length (bytes)

32

Port 1 alarm status

0x00: Disabled

0x01: Normal

0x02: Alarm

 

33

Port 2 alarm status

0x00: Disabled

0x01: Normal

0x02: Alarm

 

34

Ports 3 to 128 alarm status

Each port occupies 1 byte

0x01: Normal

0x02: Alarm

 

160

Temperature alarm status

0x01: Normal

0x02: Alarm

 

161

CPU alarm status

0x01: Normal

0x02: Alarm

 

162

Memory alarm status

0x01: Normal

0x02: Alarm

 

163

Power supply alarm status

0x01: Normal

0x02: Power supply 1 alarm

0x03: Power supply 2 alarm

 

164 to 199

Reserved

 

 

 

 

 

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Intelligent Storage
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
  • Technical Blogs
All Support
  • Become A Partner
  • Partner Policy & Program
  • Global Learning
  • Partner Sales Resources
  • Partner Business Management
  • Service Business
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us
新华三官网