04-Interface
HomeSupportWirelessWX3800X Series Access ControllersReference GuidesMIB CompanionH3C Wireless Products MIB Reference(R14xx R12xx)-6W10004-Interface
01-HH3C-IF-EXT-MIB
01-HH3C-IF-EXT-MIB 1.10 MB
HH3C-IF-EXT-MIB· 1
About this MIB· 1
MIB file name· 1
Root object 1
Scalar objects· 1
hh3cIfShutDownInterval (1.3.6.1.4.1.25506.2.40.1.2) 1
hh3cIfCurrentUsedRatio (1.3.6.1.4.1.25506.2.40.30.0) 1
hh3cIfUsedRatioThershold (1.3.6.1.4.1.25506.2.40.31.0) 1
hh3cIfDiscardType (1.3.6.1.4.1.25506.2.40.32.0) 1
hh3cIfDiscardThreshold (1.3.6.1.4.1.25506.2.40.33.0) 2
Tabular objects· 2
hh3cIfFlowStatTable· 2
hh3cIfSpeedStatTable· 3
hh3cIfHCFlowStatTable· 3
hh3cRTParentIfTable· 4
hh3cRTSubIfTable· 5
hh3cIfLinkModeTable· 5
hh3cIfPortTypeTable· 6
hh3cIfTable· 7
hh3cIfUsingTable· 7
hh3cIfPfcDot1pTable· 8
Notifications· 9
hh3cIfPortUp· 9
hh3cIfPortDown· 10
hh3cIfMonInputUsageRising· 11
hh3cIfMonInputUsageResume· 12
hh3cIfMonOutputUsageRising· 13
hh3cIfMonOutputUsageResume· 14
hh3cIfMonInputErrorAlarmRising· 15
hh3cIfMonInputErrorAlarmResume· 16
hh3cIfMonOutputErrorAlarmRising· 17
hh3cIfMonOutputErrorAlarmResume· 18
hh3cIfMonSdhErrorRising· 19
hh3cIfMonSdhErrorResume· 21
hh3cIfMonSdhB1ErrorRising· 22
hh3cIfMonSdhB1ErrorResume· 23
hh3cIfMonSdhB2ErrorRising· 24
hh3cIfMonSdhB2ErrorResume· 25
hh3cIfMonCRCErrorRising· 26
hh3cIfMonCRCErrorResume· 28
hh3cIfMonRxPauseFrameRising· 29
hh3cIfMonRxPauseFrameResume· 30
hh3cIfMonTxPauseFrameRising· 31
hh3cIfMonTxPauseFrameResume· 32
hh3cIfMonGiantRising· 33
hh3cIfMonGiantResume· 34
hh3cIfMonRuntRising· 35
hh3cIfMonRuntResume· 37
hh3cIfPfcOutRising· 38
hh3cIfInPfcRising· 39
hh3cIfPortRateDegrade· 40
hh3cIfPortRateDegradeResume· 41
hh3cIfBufferInDiscardAlarm·· 41
hh3cIfBufferInDiscardResume· 42
hh3cIfHalfDuplexRising· 43
hh3cIfChangeMultiChassis· 43
hh3cIfChangeMultiChassisResume· 44
hh3cIfCfgRecoverOverSlot 45
hh3cIfCfgRecoverOverSubSlot 46
hh3cIfInterfaceDelete· 46
hh3cIfErrordown· 47
hh3cIfErrordownRecovery· 49
hh3cIfLosAlarm·· 50
hh3cIfLosAlarmResume· 51
hh3cIfLofAlarm·· 52
hh3cIfLofAlarmResume· 53
hh3cIfLFaultAlarm·· 54
hh3cIfLFaultAlarmResume· 54
hh3cIfRFaultAlarm·· 55
hh3cIfRFaultAlarmResume· 56
hh3cIfOofAlarm·· 57
hh3cIfOofAlarmResume· 58
hh3cIfSfbereAlarm·· 59
hh3cIfSfbereAlarmResume· 60
hh3cIfPaisAlarm·· 60
hh3cIfPaisAlarmResume· 61
hh3cIfHpJ1TiuAlarm·· 62
hh3cIfHpJ1TiuAlarmResume· 63
hh3cIfRroolAlarm·· 64
hh3cIfRroolAlarmResume· 65
hh3cIfNegoFailedAlarm·· 65
hh3cIfNegoFailedAlarmResume· 66
hh3cIfEthRxFlowFallAlarm·· 67
hh3cIfEthRxFlowFallAlarmResume· 68
hh3cIfEthTxFlowFallAlarm·· 68
hh3cIfEthTxFlowFallAlarmResume· 69
hh3cIfLoopbackAlarm·· 70
hh3cIfLoopbackAlarmResume· 71
hh3cIfTtlLoop· 71
hh3cIfTtlLoopResume· 72
hh3cIfHalfDuplexClear 74
hh3cIfEgressDropAlarm·· 74
hh3cIfEgressDropRecover 75
hh3cIfBoardEgressDropAlarm·· 76
hh3cIfBoardEgressDropRecover 77
hh3cIfComboTypeChange· 77
hh3cIfIngressAgingDropAlarm·· 78
hh3cIfIngressAgingDropResume· 79
hh3cIfMonInputJamDiscardAlarm·· 80
hh3cIfMonInputJamDiscardResume· 81
hh3cIfMonOutputJamDiscardAlarm·· 82
hh3cIfMonOutputJamDiscardResume· 83
hh3cIfMonPktDropRateRising· 84
hh3cIfMonPktDropRateRecover 85
hh3cIfMonBadBytesErrorRising· 86
hh3cIfMonBadBytesErrorResume· 87
hh3cIfMonPortCrcRateExceed· 88
hh3cIfMonPortErrorRateExceed· 89
hh3cIfMonInBCRapidChange· 90
hh3cIfMonInBCRapidRecover 91
hh3cIfFlowControlDLAlarm·· 92
hh3cIfFlowControlDLAlarmResume· 93
hh3cIfOutputErrorAlarm·· 93
hh3cIfOutputErrorAlarmResume· 94
hh3cIfCableSnrAbnormal 95
hh3cIfCableSnrNormal 96
hh3cIfCableSnrDetectNotSupport 97
hh3cIfSfpNotSupportSingleFiber 97
hh3cIfLRMStateAbnormal 98
hh3cIfSfpWorkOnlyNonNego· 99
hh3cIfPfcDeadLockAlarm·· 100
hh3cIfPfcDeadLockResume· 101
hh3cIfPfcTurnOffAlarm·· 101
hh3cIfPfcTurnOffResume· 102
hh3cIfQueueAlarm·· 103
hh3cIfQueueResume· 104
hh3cIfQueueStatDiscardAlarm·· 105
hh3cIfQueueStatDiscardResume· 106
hh3cIfQueueEgressCongestionAlarm·· 107
hh3cIfQueueEgressCongestionClear 108
HH3C-IF-EXT-MIB
About this MIB
Use this MIB to manage and describe interfaces.
MIB file name
hh3c-if-ext.mib
Root object
iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).hh3c(25506).hh3cCommon(2).hh3cIfExt(40)
Scalar objects
Object (OID)
Access
Value range
Implementation
read-write
Integer32
Integer32(1..2147483647)
Port status detection timer.
0..300
Object (OID)
Access
Value range
Implementation
accessible-for-notify
Unsigned32
Unsigned32 (0..4294967295)
Current queue usage
As per the MIB.
Object (OID)
Access
Value range
Implementation
Unsigned32
Queue usage threshold
As per the MIB.
Object (OID)
Access
Value range
Implementation
INTEGER
discardstat(1)
discardByte(2)
discardrate(3)
Packet loss type
As per the MIB.
Object (OID)
Access
Value range
Implementation
Counter64
Counter64
(0..18446744073709551615)
Packet loss threshold
As per the MIB.
Tabular objects
hh3cIfFlowStatTable
About this table
Use this table to obtain the interface traffic information.
Support for operations
CreateNot supported
Edit/ModifyNot supported
DeleteNot supported
ReadSupported
Columns
The table index is ifIndex.
Object (OID)
Access
Value range
Implementation
hh3cIfStatFlowInterval (1.3.6.1.4.1.25506.2.40.2.1.2.1.1.1)
read-write
Integer32
Integer32(1..300)
Traffic statistics polling interval.
Implementation varies by product.
hh3cIfStatFlowInBits (1.3.6.1.4.1.25506.2.40.2.1.2.1.1.2)
read-only
Unsigned32
Incoming traffic in bits.
As per the MIB.
hh3cIfStatFlowOutBits (1.3.6.1.4.1.25506.2.40.2.1.2.1.1.3)
read-only
Unsigned32
Outgoing traffic in bits.
As per the MIB.
hh3cIfStatFlowInPkts (1.3.6.1.4.1.25506.2.40.2.1.2.1.1.4)
read-only
Unsigned32
Incoming traffic in packets.
As per the MIB.
hh3cIfStatFlowOutPkts (1.3.6.1.4.1.25506.2.40.2.1.2.1.1.5)
read-only
Unsigned32
Outgoing traffic in packets.
As per the MIB.
hh3cIfStatFlowInBytes (1.3.6.1.4.1.25506.2.40.2.1.2.1.1.6)
read-only
Unsigned32
Incoming traffic in bytes.
As per the MIB.
hh3cIfStatFlowOutBytes (1.3.6.1.4.1.25506.2.40.2.1.2.1.1.7)
read-only
Unsigned32
Outgoing traffic in bytes.
As per the MIB.
About this table
Use this table to obtain the interface traffic speed statistics.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cIfSpeedStatInterval (1.3.6.1.4.1.25506.2.40.2.1.2.2.1.1)
read-write
Integer32
Integer32(1..300)
Interface traffic speed statistics polling interval. 0 indicates the interface traffic speed statistics collection feature is disabled.
About this table
Use this table to obtain the 64-bit traffic information of interfaces.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cIfStatFlowHCInBits (1.3.6.1.4.1.25506.2.40.2.1.2.3.1.1)
read-only
CounterBasedGauge64
Counter64 (0..18446744073709551615)
Incoming traffic in bits (64-bit version).
As per the MIB.
hh3cIfStatFlowHCOutBits (1.3.6.1.4.1.25506.2.40.2.1.2.3.1.2)
read-only
CounterBasedGauge64
Outgoing traffic in bits (64-bit version).
As per the MIB.
hh3cIfStatFlowHCInPkts (1.3.6.1.4.1.25506.2.40.2.1.2.3.1.3)
read-only
CounterBasedGauge64
Incoming traffic in packets (64-bit version).
As per the MIB.
hh3cIfStatFlowHCOutPkts (1.3.6.1.4.1.25506.2.40.2.1.2.3.1.4)
read-only
CounterBasedGauge64
Outgoing traffic in packets (64-bit version).
As per the MIB.
hh3cIfStatFlowHCInBytes (1.3.6.1.4.1.25506.2.40.2.1.2.3.1.5)
read-only
CounterBasedGauge64
Incoming traffic in bytes (64-bit version).
As per the MIB.
hh3cIfStatFlowHCOutBytes (1.3.6.1.4.1.25506.2.40.2.1.2.3.1.6)
read-only
CounterBasedGauge64
Outgoing traffic in bytes (64-bit version).
As per the MIB.
hh3cRTParentIfTable
About this table
Use this table to obtain main interface information of subinterfaces.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cRTParentIfIndex (1.3.6.1.4.1.25506.2.40.2.2.1.1.1)
not-accessible
Integer32
Main interface index. Index of the interface for which you can create subinterfaces.
As per the MIB.
hh3cRTMinSubIfOrdinal (1.3.6.1.4.1.25506.2.40.2.2.1.1.2)
read-only
Integer32
Minimum number of the subinterface that can be created.
As per the MIB.
hh3cRTMaxSubIfOrdinal (1.3.6.1.4.1.25506.2.40.2.2.1.1.3)
read-only
Integer32
Maximum number of the subinterface that can be created.
As per the MIB.
hh3cRTSubIfTable
About this table
Use this table to obtain information about subinterface information of main interfaces.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
The table index is hh3cRTSubIfParentIfIndex.
Object (OID)
Access
Value range
Implementation
hh3cRTSubIfParentIfIndex (1.3.6.1.4.1.25506.2.40.2.2.2.1.1)
not-accessible
Integer32
As per the MIB.
hh3cRTSubIfOrdinal (1.3.6.1.4.1.25506.2.40.2.2.2.1.2)
not-accessible
Integer32
Subinterface number.
As per the MIB.
hh3cRTSubIfSubIfIndex (1.3.6.1.4.1.25506.2.40.2.2.2.1.3)
read-only
Integer32
Subinterface index.
As per the MIB.
hh3cRTSubIfSubIfDesc (1.3.6.1.4.1.25506.2.40.2.2.2.1.4)
read-only
DisplayString
OCTET STRING(0..255)
Subinterface description.
As per the MIB.
hh3cRTSubIfRowStatus (1.3.6.1.4.1.25506.2.40.2.2.2.1.5)
read-create
RowStatus
active(1),
notInService(2),
notReady(3),
createAndGo(4),
createAndWait(5),
destroy(6)
Subinterface state.
Available values are active(1), createAndGo(4), and destroy(6).
hh3cIfLinkModeTable
About this table
Use this table to obtain the interface link mode.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
The table index is hh3cIfLinkModeIndex.
Object (OID)
Access
Value range
Implementation
hh3cIfLinkModeIndex (1.3.6.1.4.1.25506.2.40.2.2.3.1.1)
not-accessible
Integer32
1..2147483647
Link mode index.
As per the MIB.
hh3cIfLinkMode (1.3.6.1.4.1.25506.2.40.2.2.3.1.2)
read-write
INTEGER
bridgeMode(1),
routeMode(2)
Current link mode of the interface.
As per the MIB.
hh3cIfLinkModeSwitchSupport (1.3.6.1.4.1.25506.2.40.2.2.3.1.3)
read-only
TruthValue
true(1),
false(2)
Whether the link mode of the interface can be switched.
As per the MIB.
hh3cIfPortTypeTable
About this table
Use this table to obtain the port type of an interface.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
The table index is hh3cIfPortTypeIndex.
Object (OID)
Access
Value range
Implementation
hh3cIfPortTypeIndex (1.3.6.1.4.1.25506.2.40.2.2.4.1.1)
not-accessible
Integer32
Interface index, which is the same as ifIndex in ifTable.
As per the MIB.
hh3cIfPortType (1.3.6.1.4.1.25506.2.40.2.2.4.1.2)
read-write
INTEGER
other(1),ethernet(2),fc(3)
Ethernet/ FC mode of an interface.
As per the MIB.
hh3cIfTable
About this table
Use this table to obtain interface-related information.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
The table index is hh3cIfUpDownTimes.
Object (OID)
Access
Value range
Implementation
hh3cIfUpDownTimes (1.3.6.1.4.1.25506.2.40.2.3.2.1.1)
read-only
Integer32
Number of interface up/down events.
As per the MIB.
hh3cIfMtu (1.3.6.1.4.1.25506.2.40.2.3.2.1.2)
read-write
Integer32
Interface MTU.
As per the MIB.
hh3cIfStatusKeepTime (1.3.6.1.4.1.25506.2.40.2.3.2.1.5)
read-only
TimeTicks
TimeTicks (0..4294967295)
Duration of the current interface state.
As per the MIB.
hh3cIfPfcStatus (1.3.6.1.4.1.25506.2.40.2.3.2.1.11)
read-write
INTEGER
enable(1),
disable(2),
auto(3)
PFC mode of an interface.
hh3cIfPfcDot1pNoDrop (1.3.6.1.4.1.25506.2.40.2.3.2.1.12)
read-write
BITS
pri0(0), pri1(1), pri2(2), pri3(3), pri4(4), pri5(5), pri6(6), pri7(7)
802.1p priority list for PFC on an interface.
hh3cIfDescription (1.3.6.1.4.1.25506.2.40.2.3.2.1.13)
read-write
DisplayString
Description of an interface.
As per the MIB.
hh3cIfFwdErrDiscards
(1.3.6.1.4.1.25506.2.40.2.3.2.1.14)
read-only
Unsigned32
Number of packets dropped because of forwarding entry errors on an interface.
As per the MIB.
hh3cIfUsingTable
About this table
Use this table to obtain information about breakout interfaces.
CreateNot supported
DeleteNot supported
ReadSupported
Columns
The table index is hh3cIfUsingIndex.
Object (OID)
Access
Value range
Implementation
hh3cIfUsingIndex (1.3.6.1.4.1.25506.2.40.2.3.3.1.1)
not-accessible
Integer32
Index of an interface that can be split or combined.
As per the MIB.
hh3cIfUsingSupportType (1.3.6.1.4.1.25506.2.40.2.3.3.1.2)
read-only
Integer32
Interface type that an interface can be split or combined into.
As per the MIB.
hh3cIfUsingType (1.3.6.1.4.1.25506.2.40.2.3.3.1.3)
read-write
INTEGER
noUsing(0),
using10GE(1),
using20GE(2),
using40GE(3),
using100GE(4),
using25GE(5),
using50GE(6)
using200GE(7)
using400GE(8)
Interface type that an interface will be split or combined into.
As per the MIB.
hh3cIfUsingStatus (1.3.6.1.4.1.25506.2.40.2.3.3.1.4)
read-only
INTEGER
noUsing(0),
needReboot(1)
State of the splitting or combining operation.
As per the MIB.
hh3cIfPfcDot1pTable
About this table
About this table
CreateNot supported
DeleteNot supported
ReadSupported
Columns
Object (OID)
Access
Value range
Implementation
hh3cIfPfcDot1pValue (1.3.6.1.4.1.25506.2.40.2.2.5.1.1)
read-only
INTEGER
0-7
Interface queue priority.
As per the MIB.
hh3cIfPfcDot1pInPps (1.3.6.1.4.1.25506.2.40.2.2.5.1.2)
read-only
Unsigned32
1-4294967295
Inbound rate for a priority.
As per the MIB.
hh3cIfPfcDot1pOutPps (1.3.6.1.4.1.25506.2.40.2.2.5.1.3)
read-only
Unsigned32
1-4294967295
Outbound rate for a priority.
As per the MIB.
hh3cIfPfcDot1pInPpsThreshold (1.3.6.1.4.1.25506.2.40.2.2.5.1.4)
read-write
Unsigned32
1-4294967295
Inbound rate threshold for a priority.
As per the MIB.
hh3cIfPfcDot1pOutPpsThreshold (1.3.6.1.4.1.25506.2.40.2.2.5.1.5)
read-write
Unsigned32
1-4294967295
Outbound rate threshold for a priority.
As per the MIB.
Notifications
hh3cIfPortUp
Basic information
OID
Event
Severity
Recovery notification
Default status
1.3.6.1.4.1.25506.2.40.3.0.5
Link-up alarm
Recovery
Major
ON
Notification triggers
The notification is generated when physical state of the interface changes to up.
Possible reasons are:
The undo shutdown command is executed on the interface.
The interface or link failure is resolved.
The physical state of the interface comes up.
System impact
The interface can normally forward packets.
Status control
ON
CLI: snmp-agent trap enable standard linkup
OFF
CLI: undo snmp-agent trap enable standard linkup
Object
OID (object name)
Index
Value range
1.3.6.1.2.1.2.2.1.1 (ifIndex)
Interface index.
ifIndex
Integer32
Standard MIB values.
1.3.6.1.2.1.2.2.1.2 (ifDescr)
Interface description.
ifIndex
OCTET STRING
Recommended action
No action is required.
hh3cIfPortDown
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.6
Link-down alarm.
Error
Major
1.3.6.1.4.1.25506.2.40.3.0.5 (hh3cIfPortUp)
ON
The notification is generated when physical state of the interface changes to down.
The physical link of the interface is down, and the link is disconnected.
The interface is shut down.
System impact
The interface cannot normally forward packets.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
To resolve this issue:
1.Execute the display this command in interface view to identify whether the interfaces on both end are shut down. If the interfaces are shut down, execute the undo shutdown command in interface view to bring them up.
2.Identify whether the physical connection is normal (for example, whether the network cables or transceiver modules are firmly connected). If the physical connection is abnormal, correctly connect the interfaces.
3.If the issue persists, contact H3C Support.
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.1
Inbound bandwidth usage rising alarm.
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.2 (hh3cIfMonInputUsageResume)
ON
The notification is generated when the inbound bandwidth usage exceeds the upper threshold.
System impact
When the inbound bandwidth usage reaches about 100%, the service traffic might be delayed or dropped.
Status control
ON
CLI: snmp-agent trap enable ifmonitor input-usage
OFF
CLI: undo snmp-agent trap enable ifmonitor input-usage
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.1 (hh3cIfMonInputUsageLowThres)
Lower threshold for the inbound bandwidth usage.
Unsigned32
0-100
1.3.6.1.4.1.25506.2.40.5.2.1.1.2 (hh3cIfMonInputUsageHighThres)
Upper threshold for the inbound bandwidth usage.
Unsigned32
0-100
1.3.6.1.4.1.25506.2.40.5.1.1.1.1 (hh3cIfMonInputUsageStatistics)
Inbound bandwidth usage statistics.
hh3cIfMonInputRateStatistics
Counter64
Recommended action
1.Identify whether the upper threshold set on the interface is too low.
  - If the threshold is too low, execute the port ifmonitor input-usage command to modify the threshold.
  - If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
Inbound bandwidth usage recovery alarm
Recovery
Warning
ON
The notification is generated when the inbound bandwidth usage drops from above the upper threshold to below the lower threshold.
System impact
The service restores.
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
0-100
Unsigned32
0-100
Counter64
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.3
Outbound bandwidth usage rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.4 (hh3cIfMonOutputUsageResume)
ON
The notification is generated when the outbound bandwidth usage exceeds the upper threshold.
System impact
When the outbound bandwidth usage reaches about 100%, the service traffic might be delayed or dropped.
Status control
ON
CLI: snmp-agent trap enable ifmonitor output-usage
OFF
CLI: undo snmp-agent trap enable ifmonitor output-usage
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.3 (hh3cIfMonOutputUsageLowThres)
Lower threshold for the outbound bandwidth usage.
Unsigned32
0-100
1.3.6.1.4.1.25506.2.40.5.2.1.1.4 (hh3cIfMonOutputUsageHighThres)
Upper threshold for the outbound bandwidth usage.
Unsigned32
0-100
1.3.6.1.4.1.25506.2.40.5.1.1.1.2 (hh3cIfMonOutputUsageStatistics)
Outbound bandwidth usage statistics.
Counter64
Recommended action
  - If the threshold is too low, execute the port ifmonitor output-usage command to modify the threshold.
Basic information
OID
Event
Severity
Default status
Outbound bandwidth usage recovery alarm
Recovery
Warning
ON
The notification is generated when the outbound bandwidth usage drops from above the upper threshold to below the lower threshold.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
0-100
Unsigned32
0-100
Counter64
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.5
Inbound error packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.6 (hh3cIfMonInputErrorAlarmResume)
ON
The notification is generated when the number of inbound error packets exceeds the upper threshold within the specified interval.
The optical transceiver module fails.
The optical fiber or link fails.
System impact
Service traffic might be dropped.
Status control
ON
CLI: snmp-agent trap enable ifmonitor input-error
OFF
CLI: undo snmp-agent trap enable ifmonitor input-error
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.6 (hh3cIfMonInputErrorAlarmHighThres)
Upper threshold for the number of inbound error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.5 (hh3cIfMonInputErrorAlarmLowThres)
Lower threshold for the number of inbound error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.3 (hh3cIfMonInputErrorAlarmStatistics)
Inbound error alarm statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.7 (hh3cIfMonInputErrorAlarmInterval)
Inbound error alarm statistics collection interval.
Unsigned32
0-65535
Recommended action
1.Replace the transceiver module. Identify whether the alarm is cleared.
2.Replace the optical fiber or link. Identify whether the alarm is cleared.
3.Identify whether the upper threshold set on the interface is too low.
  - If the threshold is too low, execute the port ifmonitor input-error command to modify the threshold.
Basic information
OID
Event
Severity
Default status
Inbound error packet recovery alarm
Recovery
Warning
ON
The notification is generated when the number of inbound error packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
CLI: undo snmp-agent trap enable ifmonitor input -error
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.7
Outbound error packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.8 (hh3cIfMonOutputErrorAlarmResume)
ON
The notification is generated when the number of outbound error packets exceeds the upper threshold within the specified interval.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor output-error
OFF
CLI: undo snmp-agent trap enable ifmonitor output-error
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.9 (hh3cIfMonOutputErrorAlarmHighThres)
Upper threshold for the number of outbound error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.8 (hh3cIfMonOutputErrorAlarmLowThres)
Lower threshold for the number of outbound error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.4 (hh3cIfMonOutputErrorAlarmStatistics)
Outbound error alarm statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.10 (hh3cIfMonOutputErrorAlarmInterval)
Outbound error alarm statistics collection interval.
Unsigned32
0-65535
Recommended action
1.Verify that the optical fiber is firmly installed. Identify whether the alarm is cleared.
2.Verify that the physical link is normal.
3.Execute the display interface command to identify whether the Tx power of the transceiver module of the interface that fails is within the normal range. Identify whether the negotiation mode, clock mode, and scrambling mode (link protocol, clock, and scramble) are the same on both ends. If they are different, modify the negotiation mode configuration on both ends to make them consistent. Identify whether the alarm is cleared.
4.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the port ifmonitor output-error command to modify the threshold.
5.If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
Outbound error packet recovery alarm
Recovery
Warning
ON
The notification is generated when the number of outbound error packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.9
SDH error packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.10 (hh3cIfMonSdhErrorResume)
ON
The notification is generated when the number of SDH error packets exceeds the upper threshold within the specified interval.
The optical fiber fails.
System impact
Status control
ON
Syntax: snmp-agent trap enable ifmonitor sdh-error
OFF
CLI: undo snmp-agent trap enable ifmonitor sdh-error
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.11 (hh3cIfMonSdhErrorLowThres)
Lower threshold for the number of SDH error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.12 (hh3cIfMonSdhErrorHighThres)
Upper threshold for the number of SDH error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.5 (hh3cIfMonSdhErrorStatistics)
SDH error statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.13 (hh3cIfMonSdhErrorInterval)
SDH error statistics collection interval.
Unsigned32
0-65535
Recommended action
2.Replace the optical fiber. Identify whether the alarm is cleared.
3.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the port ifmonitor sdh-error command to modify the threshold.
4.Collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
SDH error packet recovery alarm
Recovery
Warning
ON
The notification is generated when the number of SDH error packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor sdh-error
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.11
SDH B1 error packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.12 (hh3cIfMonSdhB1ErrorResume)
ON
The notification is generated when the number of SDH B1 error packets exceeds the upper threshold within the specified interval.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor sdh-b1-error
OFF
CLI: undo snmp-agent trap enable ifmonitor sdh-b1-error
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.14 (hh3cIfMonSdhB1ErrorLowThres)
Lower threshold for the number of SDH B1 error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.15 (hh3cIfMonSdhB1ErrorHighThres)
Upper threshold for the number of SDH B1 error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.6 (hh3cIfMonSdhB1ErrorStatistics)
SDH B1 error packet statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.16 (hh3cIfMonSdhB1ErrorInterval)
SDH B1 error statistics collection interval.
Unsigned32
0-65535
Recommended action
1.Identify whether the link (including optical fiber, transceiver module, transmission device, jumper, and so on) fails. Replace the faulty components (if any), and verify that the link is connected correctly. Identify whether the alarm is cleared.
2.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the port ifmonitor sdh-b1-error command to modify the threshold.
3.Collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
SDH B1 error packet recovery alarm
Recovery
Warning
ON
The notification is generated when the number of SDH B1 error packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.13
SDH B2 error packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.14 (hh3cIfMonSdhB2ErrorResume)
ON
The notification is generated when the number of SDH B2 error packets exceeds the upper threshold within the specified interval.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor sdh-b2-error
OFF
CLI: undo snmp-agent trap enable ifmonitor sdh-b2-error
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.17 (hh3cIfMonSdhB2ErrorLowThres)
Lower threshold for the number of SDH B2 error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.18 (hh3cIfMonSdhB2ErrorHighThres)
Upper threshold for the number of SDH B2 error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.7 (hh3cIfMonSdhB2ErrorStatistics)
SDH B2 error packet statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.19 (hh3cIfMonSdhB2ErrorInterval)
SDH B2 error statistics collection interval.
Unsigned32
0-65535
Recommended action
2.Replace the faulty components (if any), and verify that the link is connected correctly. Identify whether the alarm is cleared.
3.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the port ifmonitor sdh-b2-error command to modify the threshold. If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
Recovery
Warning
ON
The notification is generated when the number of SDH B2 error packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
SDH B2 error statistics.
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.15
CRC error packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.16 (hh3cIfMonCRCErrorResume)
ON
The notification is generated when the number of CRC error packets exceeds the upper threshold within the specified interval.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor crc-error
OFF
CLI: undo snmp-agent trap enable ifmonitor crc-error
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.21 (hh3cIfMonCRCErrorHighThres)
Upper threshold for the number of CRC error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.20 (hh3cIfMonCRCErrorLowThres)
Lower threshold for the number of CRC error packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.8 (hh3cIfMonCRCErrorStatistics)
CRC error statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.22 (hh3cIfMonCRCErrorInterval)
CRC error statistics collection interval.
Unsigned32
0-65535
1.3.6.1.4.1.25506.2.40.5.2.1.1.23 (hh3cIfMonCRCErrType)
INTEGER
1-2
Recommended action
3.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the port ifmonitor crc-error command to modify the threshold. If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
CRC error packet recovery alarm
Recovery
Warning
ON
The notification is generated when the number of CRC error packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
INTEGER
1-2
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.17
Received pause frame rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.18 (hh3cIfMonRxPauseFrameResume)
ON
The notification is generated when the number of received pause frames exceeds the upper threshold within the specified interval.
The rate of received pause frames exceeds the threshold.
Pause frames are received continuously for a long period of time.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor rx-pause
OFF
CLI: undo snmp-agent trap enable ifmonitor rx-pause
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.25 (hh3cIfMonRxPauseFrameHighThres)
Upper threshold for received pause frames.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.24 (hh3cIfMonRxPauseFrameLowThres)
Lower threshold for received pause frames.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.9 (hh3cIfMonRxPauseFrameStatistics)
Received pause frame statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.26 (hh3cIfMonRxPauseFrameInterval)
Received pause frame statistics collection interval.
Unsigned32
0-65535
Recommended action
1.Decrease the service traffic received on the peer interface. Identify whether the alarm is cleared.
2.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the port ifmonitor rx-pause command to modify the threshold. If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
Received pause frame recovery alarm
Recovery
Warning
ON
The notification is generated when the number of received pause frames drops from above the upper threshold to below the lower-threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.26 (hh3cIfMonRxPauseFrameHighThres)
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.25 (hh3cIfMonRxPauseFrameLowThres)
Unsigned32
1-4294967295
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.27 (hh3cIfMonRxPauseFrameInterval)
Unsigned32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.19
Transmitted pause frame rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.20 (hh3cIfMonTxPauseFrameResume)
ON
The notification is generated when the number of transmitted pause frames exceeds the upper threshold within the specified interval.
The rate of sent pause frames exceeds the threshold.
Pause frames are sent continuously for a long period of time.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor tx-pause
OFF
CLI: undo snmp-agent trap enable ifmonitor tx-pause
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.29 (hh3cIfMonTxPauseFrameHighThres)
Upper threshold for transmitted pause frames.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.28 (hh3cIfMonTxPauseFrameLowThres)
Lower threshold for transmitted pause frames.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.10 (hh3cIfMonTxPauseFrameStatistics)
Transmitted pause frame statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.29 (hh3cIfMonTxPauseFrameInterval)
Transmitted pause frame statistics collection interval.
Unsigned32
0-65535
Recommended action
1.Decrease the service traffic sent on the peer interface. Identify whether the alarm is cleared.
2.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the port ifmonitor tx-pause command to modify the threshold. If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
Transmitted pause frame recovery alarm
Recovery
Warning
ON
The notification is generated when the number of transmitted pause frames drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.21
Giant packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.22 (hh3cIfMonGiantResume)
ON
The notification is generated when the number of giant packets exceeds the upper threshold within the specified interval.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor giant
OFF
CLI: undo snmp-agent trap enable ifmonitor giant
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.30 (hh3cIfMonGiantLowThres)
Lower threshold for giant packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.31 (hh3cIfMonGiantHighThres)
Upper threshold for giant packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.11 (hh3cIfMonGiantStatistics)
Giant packet statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.32 (hh3cIfMonGiantInterval)
Giant packet statistics collection interval.
Unsigned32
0-65535
Recommended action
1.Verify that the source traffic is normal.
2.Execute the jumboframe enable command to adjust the maximum size of a packet that can be transmitted on the interface.
Basic information
OID
Event
Severity
Default status
Giant packet recovery alarm
Recovery
Warning
ON
The notification is generated when the number of giant packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
hh3cIfMonRuntRising
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.23
Runt packet rising alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.24 (hh3cIfMonRuntResume)
ON
The notification is generated when the number of runt packets exceeds the upper threshold within the specified interval.
System impact
Status control
ON
CLI: snmp-agent trap enable ifmonitor runt
OFF
CLI: undo snmp-agent trap enable ifmonitor runt
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.2.1.1.33 (hh3cIfMonRuntLowThres)
Lower threshold for runt packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.34 (hh3cIfMonRuntHighThres)
Upper threshold for runt packets.
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.5.1.1.1.12 (hh3cIfMonRuntStatistics)
Runt packet statistics.
Counter64
1-4294967295
1.3.6.1.4.1.25506.2.40.5.2.1.1.35 (hh3cIfMonRuntInterval)
Runt packet statistics collection interval.
Unsigned32
0-65535
Recommended action
hh3cIfMonRuntResume
Basic information
OID
Event
Severity
Default status
Runt packet recovery alarm
Recovery
Warning
ON
The notification is generated when the number of runt packets drops from above the upper threshold to below the lower threshold within the specified interval.
System impact
Status control
ON
OFF
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Unsigned32
1-4294967295
Unsigned32
1-4294967295
Counter64
1-4294967295
Unsigned32
0-65535
Recommended action
hh3cIfPfcOutRising
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.7
Outbound PFC frame rate rising alarm
Informational
Warning
ON
This notification is generated when the outbound PFC frame rate exceeds the early warning threshold.
System impact
Outbound PFC frames might be lost.
Status control
This notification cannot be turned off.
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.2.2.5.1.1 (hh3cIfPfcDot1pValue)
INTEGER
0-7
1.3.6.1.4.1.25506.2.40.2.2.5.1.3 (hh3cIfPfcDot1pOutPps)
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.2.2.5.1.5 (hh3cIfPfcDot1pOutPpsThreshold)
Unsigned32
1-4294967295
Recommended action
1.Identify whether the upper threshold set on the interface is too low. If the threshold is set reasonably, identify whether the interface fails.
  - If the inbound PFC frame rate exceeds the threshold, identify whether the peer device fails.
  - If the outbound PFC frame rate exceeds the threshold, identify whether the local device fails.
  - If both the inbound PFC frame rate and outbound PFC frame rate exceed the thresholds, identify whether the local device and peer device fail.
2.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the priority-flow-control early-warning dot1p dot1p-list outpps pps-value command to modify the threshold. If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
hh3cIfInPfcRising
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.8
Inbound PFC frame rate rising alarm
Informational
Warning
ON
This notification is generated when the inbound PFC frame rate exceeds the early warning threshold.
System impact
Incoming PFC frames might be lost.
Status control
Object
OID (object name)
Index
Value range
Interface index.
Integer32
OCTET STRING
INTEGER
0-7
1.3.6.1.4.1.25506.2.40.2.2.5.1.2 (hh3cIfPfcDot1pInPps)
Unsigned32
1-4294967295
1.3.6.1.4.1.25506.2.40.2.2.5.1.4 (hh3cIfPfcDot1pInPpsThreshold)
Unsigned32
1-4294967295
Recommended action
1.Identify whether the upper threshold set on the interface is too low. If the threshold is set reasonably, identify whether the device fails.
2.Identify whether the upper threshold set on the interface is too low. If the threshold is too low, execute the priority-flow-control early-warning dot1p dot1p-list inpps pps-value command to modify the threshold. If the threshold is set reasonably, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.11
Negotiated port rate degrade alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.12 (hh3cIfPortRateDegradeResume)
ON
This notification is generated when the negotiated port rate degrades.
System impact
Status control
This notification cannot be disabled.
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.1.5 (hh3cIfRate)
Actual interface bandwidth.
N/A
Unsigned32
Recommended action
1.Identify whether the link fails. If the link fails, remove the link failure and identify whether the alarm is cleared.
2.Identify whether the copper port on the peer device fails. If the copper port on the peer device fails, remove the failure and identify whether the alarm is cleared.
Basic information
OID
Event
Severity
Default status
Negotiated port rate recovery alarm
Recovery
Warning
ON
This notification is generated when the negotiated port rate recovers.
System impact
The system is not impacted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
N/A
Unsigned32
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.14
Traffic in the ingress buffer of a card is dropped
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.15 (hh3cIfBufferInDiscardResume)
ON
This notification is generated when the traffic in the ingress buffer of a card is dropped.
System impact
Traffic in the ingress buffer of a card is dropped. The inbound traffic of the card exceeds the link bandwidth of the switching fabric module.
Status control
Object
OID (object name)
Index
Value range
1.3.6.1.4.1.25506.2.40.1.6 (hh3cIfChassisIndex)
Chassis index.
N/A
Integer32
0-65535
1.3.6.1.4.1.25506.2.40.1.7 (hh3cIfSlotIndex)
Card index.
N/A
Integer32
0-65535
Recommended action
Optimize the network, and adjust the traffic forwarding solution.
Basic information
OID
Event
Severity
Default status
The uplink traffic of a card recovers from the drop state.
Recovery
Warning
ON
This notification is generated when network congestion is relieved within the specified time.
System impact
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.16
An interface operates in half duplex mode
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.52 (hh3cIfHalfDuplexClear)
ON
This notification is generated when an interface operates in half duplex mode.
System impact
Packets might be lost when an interface operates in half duplex mode.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
Configure the interface to operate in full duplex mode. Related command: duplex full.
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.17
Interface information changes when a single-chassis device is expanded to a multi-chassis device
Informational
Informational
1.3.6.1.4.1.25506.2.40.3.0.18 (hh3cIfChangeMultiChassisResume)
ON
This notification is generated if interface information changes when a single-chassis device is expanded to a multi-chassis device.
System impact
An interface name changes from a three-tier name to a four-tier name.
Status control
Object
OID (object name)
Index
Value range
Recommended action
Basic information
OID
Event
Severity
Default status
Interface information changes when a multi-chassis device is rolled back to a single-chassis device
Informational
Informational
ON
This notification is generated if interface information changes when a multi-chassis device is rolled back to a single-chassis device.
System impact
An interface name changes from a four-tier name to a three-tier name.
Status control
Object
OID (object name)
Index
Value range
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.19
The interface card configuration recovers
Informational
Informational
ON
This notification is generated if the interface card configuration recovers.
System impact
The interface card configuration has recovered, and the interface card becomes available.
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.20
The interface subcard configuration recovers
Informational
Informational
ON
The interface subcard configuration recovers.
System impact
The interface subcard configuration has recovered, and the interface subcard becomes available.
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Slot index.
N/A
Integer32
0-65535
1.3.6.1.4.1.25506.2.40.1.8 (hh3cIfSubSlotIndex)
Subcard index.
N/A
Integer32
0-65535
Recommended action
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.21
An interface is deleted
Informational
Informational
ON
This notification is generated if an interface is deleted.
System impact
Services that depend on the interface might be impacted.
Status control
Object
OID (object name)
Index
Value range
ifIndex
OCTET STRING
Recommended action
hh3cIfErrordown
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.22
An interface enters the error-down state
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.23 (hh3cIfErrordownRecovery)
ON
An error-down event occurs when an interface is set to the ERROR DOWN state after the device detects failure. In this case, the interface cannot receive or send packets and the LED for the interface is solid off.
Too many CRC error packets are generated on the interface.
The interface flaps frequently and is unstable.
System impact
Interface traffic cannot be forwarded, and the services are interrupted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.1.9 (hh3cIfErrDownDesc)
Error-down reason description.
N/A
OCTET STRING
1: CRC error packets actively report physical down events. , 2: All serdes between interface cards and switching fabric modules fail., 3: IRF fabric configuration conflicts cause the IRF port to go down., 4: The optical powers of transceiver modules are low., 5: IRF physical interfaces receive a large number of protocol packets or IRF fabric error packets within a short period of time.,  6: STP Down, 7: The interface is shut down on the data link layer because the MACsec module has not successfully negotiated the communication encryption parameters for the interface. , 8: The interface is shut down because the unknown unicast, multicast, or broadcast traffic on the interface exceeds the corresponding upper threshold. , 9: Standby bit, 10: Loop detection, 11: Link-Aggregation interface down, 12: Monitor-Link uplink down, 13: IRF-link-down, 14: MAD Down, 15: Used by FC aggregation, 16: Tunnel-Bundle administratively down, 17: FC port security, 18: Used by the NPV feature of an FC interface, 19: Used by M-LAG MAD, 20: Used by MAC flapping, 21: ETH-rddc Down, 22: Used by CFD collaboration, 23: Used by LLDP, 24: OFP DOWN, 25: The interface is shut down on the data link layer because DLDP has detected unidirectional links on the interface, 26: Used by POSA, 27: Used by collaboration group, 28: DRNI MAD Down, 29: Link-Flap DOWN
Recommended action
1.Troubleshoot the link failures.
2.Collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
An interface recovers from the error-down state
Recovery
Warning
ON
This notification is generated when an IRF physical interface recovers from the error-down state.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
N/A
OCTET STRING
Same as that of the hh3cIfErrordown node
Recommended action
hh3cIfLosAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.24
No optical signal is input for the transceiver module and the Rx signals are lost
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.25 (hh3cIfLosAlarmResume)
ON
This notification is generated when no optical signal is input for the transceiver module and the Rx signals are lost.
The attenuation of the Rx signals is high.
The Tx signals from the remote end do not have a frame structure.
The Rx direction of the local end fails.
System impact
Service switchover or interruption might occur.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
1.If a fiber port fails:
  - Identify whether the fibers are connected incorrectly (for example, two ports at different speeds are connected), and correct the incorrect connections, if any. Identify whether the alarm is cleared.
  - Identify whether the Rx optical power of the local end is normal on NMS.
If the Rx optical power is too low, clean the optical fiber pigtail and the Rx optical interface on the line card of the local end, identify whether the flange and optical attenuator of the local end are connected correctly, and identify whether the attenuation value of the optical attenuator is too great. Connect the flange and optical attenuator correctly, and identify whether the alarm is cleared.
If the Rx optical power is too high, add an optical attenuator. Adjust the Rx optical power to the normal range. Identify whether the alarm is cleared.
  - Identify whether the Tx optical power of the remote end is normal. If the Tx optical power is normal, perform an optical fiber loopback for the line card of the local end. If the alarm is cleared on the local end, it means that the Tx signals from the remote end do not have a frame structure.
2.If a copper port fails:
  - Identify whether the cable is connected incorrectly (for example, two ports at different speeds are connected), and correct the incorrect connections, if any. Identify whether the alarm is cleared.
  - Verify that the frame format of the remote end is the same as that of the local end. Identify the alarm is cleared.
Basic information
OID
Event
Severity
Default status
Optical signals are input for the transceiver module
Recovery
Warning
ON
This notification is generated when optical signals are input for the transceiver module and the signal loss alarm is cleared
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfLofAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.26
The OOF state stays continuously for 3 ms (the Rx line does not receive correct A1A2 bytes for 24 continuous frames).
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.27 (hh3cIfLofAlarmResume)
ON
This notification is generated when the OOF state stays continuously for 3 ms (the Rx line does not receive correct A1A2 bytes for 24 continuous frames).
System impact
Services might be interrupted. The following impacts might occur:
Impact 1: After this alarm is generated, the services are interrupted, and AIS signals are inserted to the downstream devices.
Impact 2: After this alarm is generated, the system will automatically return MS_RDI alarms to the upstream devices, and the upstream devices generate MS_RDI alarms.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
Basic information
OID
Event
Severity
Default status
This recovery notification is generated when the OOF state recovers.
Recovery
Warning
ON
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfLFaultAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.28
Local end fault alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.29 (hh3cIfLFaultAlarmResume)
ON
This notification is generated on the local end when the Rx link from the remote end to the local end fails.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
1.Identify whether the Rx fiber fails.
2.Identify whether the transceiver modules of the local end and remote end fail.
3.Identify whether the interface card of the local end fails.
Basic information
OID
Event
Severity
Default status
Local end fault alarm cleared
Recovery
Warning
ON
This notification is generated when the local end fault alarm is cleared.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfRFaultAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.30
Remote end fault alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.31 (hh3cIfRFaultAlarmResume)
ON
This notification is generated on the local end when the Tx link from the local end to the remote end fails.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
1.Identify whether the Tx fiber fails.
3.Identify whether the interface card of the remote end fails.
Basic information
OID
Event
Severity
Default status
Remote end fault alarm cleared
Recovery
Warning
ON
This notification is generated when the remote end fault alarm is cleared.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfOofAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.32
When the frame alignment signal byte cannot be determined in the input bit stream, the STM-N signal is considered as in the loss of frame alignment state.
If the frame header cannot be determined for five continuous frames, the OOF alarm is generated.
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.33 (hh3cIfOofAlarmResume)
ON
When the frame alignment signal byte cannot be determined in the input bit stream, the STM-N signal is considered as in the loss of frame alignment state. If the frame header cannot be determined for five continuous frames, the OOF alarm is generated.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
1.Identify whether the fibers are connected incorrectly (for example, two ports at different speeds are connected), and correct the incorrect connections, if any.
2.Identify whether the Rx optical power of the local end is normal on NMS.
  - If the Rx optical power is too low, clean the optical fiber pigtail and the Rx optical interface on the line card of the local end, identify whether the flange and optical attenuator of the local end are connected correctly, and identify whether the attenuation value of the optical attenuator is too great. Connect the flange and optical attenuator correctly, and identify whether the alarm is cleared.
  - If the Rx optical power is too high, add an optical attenuator. Adjust the Rx optical power to the normal range. Identify whether the alarm is cleared.
3.Identify whether the Tx optical power of the remote end is normal. If the Tx optical power is normal, perform an optical fiber loopback for the line card of the local end. If the alarm is cleared on the local end, it means that the Tx signals from the remote end do not have a frame structure.
Basic information
OID
Event
Severity
Default status
Recovery
Warning
ON
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfSfbereAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.34
The regenerator section (B2) bit error rate exceeds the threshold
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.35 (hh3cIfSfbereAlarmResume)
ON
This notification is generated when the regenerator section (B2) bit error rate exceeds the threshold.
The optical fiber is unclean or the connector is incorrect, or the fiber ages.
The transmitter of the remote end fails.
The receiver of the local end fails.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
3.Execute the display interface phy-option command to identify whether the Rx optical power of the transceiver module in the faulty interface is within the normal range. Identify whether the negotiation mode, clock mode, and scrambling mode (line protocol state, clock, and scramble) are the same on both ends. If they are different, modify the negotiation mode configuration on both ends to make them consistent. Identify whether the alarm is cleared.
Basic information
OID
Event
Severity
Default status
The regenerator section (B2) bit error rate drops below the threshold
Recovery
Warning
ON
This notification is generated when the regenerator section (B2) bit error rate drops below the threshold.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfPaisAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.36
Higher-order path alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.37 (hh3cIfPaisAlarmResume)
ON
The SDH mapping mode configuration is incorrect.
System impact
The higher-order path service is interrupted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.1.17 (hh3cIfSDHHpIndex)
Higher-order path number.
N/A
Integer32
Recommended action
1.Identify whether the B1 bit error rate alarm exists and clear the alarm, if any. Identify whether this alarm is cleared.
2.Verify that the SDH mapping mode of the remote end is the same as that of the local end. Identify whether the alarm is cleared.
Basic information
OID
Event
Severity
Default status
Higher-order path alarm cleared
Recovery
Warning
ON
This notification is generated when the higher-order path alarm is cleared.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
N/A
Integer32
Recommended action
hh3cIfHpJ1TiuAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.38
Higher-order path J1 byte instability alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.39 (hh3cIfHpJ1TiuAlarmResume)
ON
This notification is generated when the higher-order path J1 byte is unstable.
The optical fiber is disconnected.
The line attenuation is too serious.
The transmitter of the remote end fails, and the line fails to transmit data.
The cross-connection card of the remote end fails or is absent.
The clock card of the remote end fails.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
N/A
Integer32
Recommended action
1.Identify whether the fiber port has optical fibers connected. If not, turn off the laser of the fiber port. Identify whether the alarm is cleared.
2.Identify whether the optical fiber of the link is broken. If yes, replace the optical fiber. Identify whether the alarm is cleared.
3.Identify whether the Rx optical power of the local end is too low. If yes, clean the optical fiber pigtail and the Rx optical interface on the interface card of the local end, identify whether the flange and optical attenuator of the local end are connected correctly, and identify whether the attenuation value of the optical attenuator is too great. Connect the flange and optical attenuator correctly, and identify whether the alarm is cleared.
4.Identify whether the Rx optical power of the local end is too high. If yes, add an optical attenuator, and adjust the Rx optical power to the normal range. Identify whether the alarm is cleared.
5.Identify whether the laser is turned off for the line card of the remote end. If yes, turn on the laser. Identify whether the alarm is cleared.
6.Check the Tx optical power of the remote end. If the Tx optical power is abnormal, replace the corresponding line card of the remote end. Identify whether the alarm is cleared.
7.Identify whether the clock card of the remote end fails. If yes, replace the clock card of the remote end. Identify whether the alarm is cleared.
8.Identify whether the Rx card of the local end fails. If yes, replace the card that outputs this alarm on the local end. Identify whether the alarm is cleared.
9.Collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
The higher-order path J1 byte becomes stable
Recovery
Warning
ON
This notification is generated when the higher-order path J1 byte becomes stable.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
N/A
Integer32
Integer32(1..2147483647)
Recommended action
hh3cIfRroolAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.40
Loss of lock for Rx reference clock
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.41 (hh3cIfRroolAlarmResume)
ON
The clock extraction module of the line card fails.
The cross-connection clock card of the remote end fails or is absent.
System impact
The line card cannot extract the valid clock from the received optical signals. As a result, the services are interrupted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
1.Identify whether the clock of the local end fails. If yes, first troubleshoot the clock failure, and then identify whether the alarm is cleared.
2.If the alarm is not cleared, identify whether the clock of the remote end fails.
Basic information
OID
Event
Severity
Default status
Loss of lock for Rx reference clock recovers
Recovery
Warning
ON
This notification is generated when the loss of lock for the Rx reference clock recovers.
System impact
The services restore.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfNegoFailedAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.42
Autonegotiation failure alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.43 (hh3cIfNegoFailedAlarmResume)
ON
This notification is generated when autonegotiation fails.
System impact
The interface cannot come up, and the link is disconnected.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
Identify whether the speed and duplex mode are consistent on both interfaces of a link.
Basic information
OID
Event
Severity
Default status
Autonegotiation recovery alarm
Recovery
Warning
ON
This notification is generated when autonegotiation successfully recovers.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfEthRxFlowFallAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.44
The inbound traffic of an Ethernet interface falls. When the interface comes up, the traffic falling monitoring flag is enabled
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.45 (hh3cIfEthRxFlowFallAlarmResume)
ON
This notification is generated if the interface comes up and the traffic falling monitoring flag is enabled.
System impact
The traffic suddenly falls.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
Basic information
OID
Event
Severity
Default status
The inbound traffic of an Ethernet interface falls. When the interface comes up, the traffic rising monitoring flag is disabled.
Recovery
Warning
ON
This notification is generated if the interface comes up and the traffic rising monitoring flag is disabled.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfEthTxFlowFallAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.46
The outbound traffic of an Ethernet interface falls. When the interface comes up, the traffic falling monitoring flag is enabled.
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.47 (hh3cIfEthTxFlowFallAlarmResume)
ON
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
Basic information
OID
Event
Severity
Default status
The outbound traffic of an Ethernet interface falls. When the interface comes up, the traffic rising monitoring flag is disabled.
Recovery
Warning
ON
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Recommended action
hh3cIfLoopbackAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.48
Loopback configuration deployment alarm
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.49 (hh3cIfLoopbackAlarmResume)
ON
This notification is generated when loopback configuration is deployed.
System impact
Loops exist in the system. If a port or channel has services, the services will be interrupted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
OCTET STRING(0..255)
1.3.6.1.4.1.25506.2.40.1.10 (hh3cIfLoopBackType)
Loopback type.
N/A
INTEGER
internal (5),, external (6)
Recommended action
Execute the undo loopback command to disable loopback on an Ethernet interface.
Basic information
OID
Event
Severity
Default status
Loopback completed
Recovery
Warning
ON
This recovery notification is generated when loopback is completed.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
0-65535
ifIndex
OCTET STRING
Loopback type.
N/A
INTEGER
noloopback(1)
Recommended action
hh3cIfTtlLoop
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.50
Loopback alarm due to TTL timeout
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.51 (hh3cIfTtlLoopResume)
ON
This notification is generated when loopback occurs due to TTL timeout.
System impact
This notification is generated mainly in Layer 3 loop detection, and does not obviously impact other services.
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Slot index.
N/A
Integer32
0-65535
1.3.6.1.4.1.25506.2.40.1.13 (hh3cIfPreDataHighByte)
Highest 32 bits in the last data.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.12 (hh3cIfPreDataLowByte)
Lowest 32 bits in the last data.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.15 (hh3cIfCurDataHighByte)
Highest 32 bits in the current data.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.14 (hh3cIfCurDataLowByte)
Lowest 32 bits in the current data.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.16 (hh3cIfIntervalTime)
Alarm interval.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.11 (hh3cIfTtlLoopThreshold)
Time threshold for the loop alarm due to TTL timeout.
N/A
Integer32
Recommended action
Identify whether Layer 3 loops exist through examining the Layer 3 forwarding entries.
hh3cIfTtlLoopResume
Basic information
OID
Event
Severity
Default status
Loop alarm due to TTL timeout cleared
Recovery
Warning
ON
This notification is generated when the loop alarm due to TTL timeout is cleared.
System impact
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Slot index.
N/A
Integer32
0-65535
N/A
Integer32
N/A
Integer32
Highest 4 bits in the current data.
N/A
Integer32
N/A
Integer32
Alarm interval.
N/A
Integer32
N/A
Integer32
Recommended action
Basic information
OID
Event
Severity
Default status
Autonegotiated full duplex mode for an interface
Recovery
Warning
ON
This notification is generated when the autonegotiated duplex mode changes from half duplex to full duplex for an interface.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
hh3cIfEgressDropAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.53
Packet drop on a port
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.54 (hh3cIfEgressDropRecover)
ON
This notification is generated when packets are dropped within the specified time.
System impact
Outgoing traffic of a port is dropped.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.2.2.6.1.1 (hh3cIfQueId)
ID of an interface's buffer queue.
hh3cIfQueId
INTEGER
que0(1),, que1(2),, que2(3),, que3(4),, que4(5),, que5(6),, que6(7),, que7(8)
Recommended action
Basic information
OID
Event
Severity
Default status
Packet drop on a port recovers
Recovery
Warning
ON
This notification is generated when packet drop recovers on a port within the specified time.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Recommended action
hh3cIfBoardEgressDropAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.55
Outgoing unicast traffic of a card is dropped
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.56 (hh3cIfBoardEgressDropRecover)
ON
This notification is generated if outgoing unicast traffic of a card is dropped within the specified time.
System impact
The outgoing unicast traffic of a card is dropped.
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
1.3.6.1.4.1.25506.2.40.1.21 (hh3cIfCpuId)
CPU ID of a card.
N/A
Unsigned32
Unsigned32 (0..4294967295)
Recommended action
Basic information
OID
Event
Severity
Recovery notification
Default status
Outgoing unicast traffic drop of a card recovers.
Recovery
Warning
ON
Notification triggers
This notification is generated if outgoing unicast traffic drop of a card recovers within the specified time.
System impact
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
CPU ID of a card.
N/A
Unsigned32
Recommended action
hh3cIfComboTypeChange
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.57
The combo type is changed by the CLI
Informational
Informational
ON
This notification is generated if the combo enable { copper | fiber } command configuration changes.
System impact
Status control
Object
OID (object name)
Index
Value range
1.3.6.1.2.1.2.2.1.1 (ifIndex)
Interface index.
ifIndex
Integer32
Standard MIB values.
1.3.6.1.2.1.2.2.1.2 (ifDescr)
Interface description.
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.1.22 (hh3cIfOldComboType)
Combo interface type before change.
N/A
INTEGER
fiber(1),, copper(2)
1.3.6.1.4.1.25506.2.40.1.23 (hh3cIfNewComboType)
Combo interface type after change.
N/A
INTEGER
Recommended action
No action is required.
hh3cIfIngressAgingDropAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.58
The traffic in the ingress buffer of a slot is dropped because of no schedule.
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.59 (hh3cIfIngressAgingDropResume)
ON
This notification is generated if the traffic of high-priority queues exceeds the port bandwidth and thus the packets in low-priority queues cannot be scheduled.
System impact
The service traffic of a card is lost.
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
CPU ID of a card.
N/A
Unsigned32
Recommended action
Basic information
OID
Event
Severity
Default status
Traffic drop in the ingress buffer of a slot recovers
Recovery
Warning
ON
This notification is generated if traffic drop in the ingress buffer of a slot recovers within the specified time.
System impact
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
CPU ID of a card.
N/A
Unsigned32
Recommended action
hh3cIfMonInputJamDiscardAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.35
The number of incoming packets dropped due to congestion exceeds the threshold
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.36 (hh3cIfMonInputJamDiscardResume)
ON
This notification is generated if the number of incoming packets dropped due to congestion exceeds the threshold.
System impact
If this alarm appears, serious congestion has occurred in the network. If you do not resolve this issue timely, network congestion will cause more packets to be dropped. As a result, services will be impacted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.1.1.1.15 (hh3cIfMonJamDiscardStatistics)
Number of packets dropped due to congestion.
hh3cIfMonInputRateStatistics
Counter64
Counter64, (0..18446744073709551615)
1.3.6.1.4.1.25506.2.40.5.2.1.1.42 (hh3cIfMonJamDiscardThres)
Threshold for the number of packets dropped due to congestion.
hh3cIfMonInputUsageLowThres
Unsigned32
1.3.6.1.4.1.25506.2.40.5.2.1.1.43 (hh3cIfMonJamDiscardInterval)
Statistics interval for the number of packets dropped due to congestion.
Unsigned32
Unsigned32 (0..65535)
Recommended action
1.Execute the display this command to identify whether rate limiting is configured in the inbound direction of the interface.
2.Execute the qos lr inbound cir cir-value [ cbs cbs-value ] command in interface view to modify the rate limit values or execute the undo qos lr inbound command to delete rate limit configuration. Identify whether the alarm is cleared.
3.According to the service conditions, execute the port ifmonitor input-usage high-threshold high-value command in interface view to modify the alarm threshold for the number of packets lost due to congestion on the interface.
Basic information
OID
Event
Severity
Default status
The number of incoming packets dropped due to congestion is restored to the normal state
Recovery
Warning
ON
This notification is generated if the number of incoming packets dropped due to congestion drops below the threshold.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Counter64
Unsigned32
Unsigned32
Recommended action
hh3cIfMonOutputJamDiscardAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.37
The number of outgoing packets dropped due to congestion exceeds the threshold
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.38 (hh3cIfMonOutputJamDiscardResume)
ON
This notification is generated if the number of outgoing packets dropped due to congestion exceeds the threshold.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Counter64
Unsigned32
Unsigned32
Recommended action
1.Execute the display this command to identify whether rate limiting is configured in the outbound direction of the interface.
2.Execute the qos lr outbound cir cir-value [ cbs cbs-value ] command in interface view to modify the rate limit values or execute the undo qos lr outbound command to delete rate limit configuration. Identify whether the alarm is cleared.
3.According to the service conditions, execute the port ifmonitor output-usage high-threshold high-value command in interface view to modify the alarm threshold for the number of packets lost due to congestion on the interface.
Basic information
OID
Event
Severity
Default status
The number of outgoing packets dropped due to congestion is restored to the normal state
Recovery
Warning
ON
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Counter64
Unsigned32
Unsigned32
Recommended action
hh3cIfMonPktDropRateRising
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.39
The number of packets dropped on an interface card exceeds the configured alarm threshold
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.40 (hh3cIfMonPktDropRateRecover)
ON
This notification is generated when the number of packets dropped on an interface card exceeds the configured alarm threshold.
System impact
The sending bandwidth of normal protocol packets is preempted. As a result, the protocols are interrupted, and data is lost.
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
CPU ID of a card.
N/A
Unsigned32
1.3.6.1.4.1.25506.2.40.1.24 (hh3cIfDropRateThreshold)
Threshold for the packet loss rate.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.25 (hh3cIfCurrentDropRate)
Current packet loss rate.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.26 (hh3cIfDropRateInterval)
Packet loss rate detection interval.
N/A
Integer32
1.3.6.1.4.1.25506.2.40.1.27 (hh3cIfMessageProtocol)
Packet protocol.
N/A
Integer32
Recommended action
1.If the shutdown keyword is specified when you configure the alarm for the number of packets lost on a card, the system shuts down all interfaces on the card when the number of lost packets on the card exceeds the upper threshold. Then, the card stops forwarding all packets. To recover the interfaces on the card, execute the undo shutdown command on the interfaces.
2.If the reboot keyword is specified when you configure the alarm for the number of packets lost on a card, the system reboots the interface card when the number of lost packets on the card exceeds the upper threshold.
Basic information
OID
Event
Severity
Default status
The number of packets dropped on an interface card is restored to the normal state
Recovery
Warning
ON
This notification is generated when the number of packets dropped on an interface card drops below the threshold within the specified time.
System impact
Status control
Object
OID (object name)
Index
Value range
Chassis index.
N/A
Integer32
0-65535
Card index.
N/A
Integer32
0-65535
CPU ID of a card.
N/A
Unsigned32
N/A
Integer32
N/A
Integer32
N/A
Integer32
Packet protocol.
N/A
Integer32
Recommended action
hh3cIfMonBadBytesErrorRising
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.41
The number of bytes in bad packets exceeds the set alarm threshold
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.42 (hh3cIfMonBadBytesErrorResume)
ON
This notification is generated when the number of bytes in bad packets exceeds the set alarm threshold within the specified time.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.1.1.1.16 (hh3cIfMonBadBytesStatistics)
Number of bytes in bad packets.
Counter64
Counter64 (0..18446744073709551615)
1.3.6.1.4.1.25506.2.40.5.2.1.1.44 (hh3cIfMonBadBytesThreshold)
Threshold for the number of bytes in bad packets.
Unsigned32
1.3.6.1.4.1.25506.2.40.5.2.1.1.45 (hh3cIfMonBadBytesDiscardInterval)
Statistics interval for the number of bytes in bad packets.
Unsigned32
Recommended action
1.When the attenuation of the line is too great, replace the optical fiber. Identify whether the alarm is cleared.
2.View the Tx optical power of the remote end on NMS. If the Tx optical power is abnormal, replace the corresponding line card of the remote end. Identify whether the recovery notification is generated.
3.Replace the line card of the local end that reports the alarm. Identify whether the recovery notification is generated.
Basic information
OID
Event
Severity
Default status
The number of bytes in bad packets is restored to the normal state
Recovery
Warning
ON
This notification is generated when the number of bytes in bad packets drops below the set alarm threshold within the specified time.
System impact
The services recover.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Counter64
Unsigned32
Unsigned32
Recommended action
hh3cIfMonPortCrcRateExceed
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.43
The CRC packet error rate is equal to or greater than 1000 pps
Informational
Warning
ON
This notification is generated when the CRC packet error rate is equal to or greater than 1000 pps within the specified time.
System impact
Some service data on the interface is dropped.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.5.1.1.1.17 (hh3cIfMonErrorRateStatistics)
Packet error rate statistics.
Counter64
1.3.6.1.4.1.25506.2.40.5.2.1.1.46 (hh3cIfMonErrorRateThres)
Threshold for the packet error rate.
Unsigned32
1.3.6.1.4.1.25506.2.40.5.2.1.1.47 (hh3cIfMonErrorRateDiscardInterval)
Statistics interval for the packet error rate.
Unsigned32
Recommended action
1.Replace the transceiver module, and then execute the display interface command to identify whether the number of CRC error packets keeps increasing on the interface.
2.Replace the fiber, and then execute the display interface command to identify whether the number of CRC error packets keeps increasing on the interface.
hh3cIfMonPortErrorRateExceed
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.44
The average packet error rate of CRC error packets, giants, and runts exceeds 1000 pps.
Informational
Warning
ON
This notification is generated when the average packet error rate of CRC error packets, giants, and runts exceeds 1000 pps within the specified time.
System impact
Some service data on the interface might be dropped.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Counter64
Unsigned32
Unsigned32
Recommended action
1.Replace the transceiver module, and then execute the display interface command to identify whether the number of error packets keeps increasing on the interface.
2.Replace the fiber, and then execute the display interface command to identify whether the number of error packets keeps increasing on the interface.
3.Execute the jumboframe enable command to modify the jumbo frame length limit or change the packet length. Then, execute the display interface command to identify whether the number of error packets keeps increasing.
4.Collect alarm information and configuration data, and then contact H3C Support.
hh3cIfMonInBCRapidChange
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.6.0.45
The inbound broadcast traffic of an interface rapidly changes to exceed the threshold
Error
Warning
1.3.6.1.4.1.25506.2.40.6.0.46 (hh3cIfMonInBCRapidRecover)
ON
This notification is generated if the inbound broadcast traffic of an interface rapidly changes to exceed the threshold (CurrentInputBroadcastRate BaseInputBroadcastRate+InputBroadcastChangeThreshold) within the specified time.
System impact
Packet loss might occur.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
1.3.6.1.4.1.25506.2.40.1.28 (hh3cIfCurrentFlowThreshold)
Current traffic threshold.
N/A
Counter64
1.3.6.1.4.1.25506.2.40.1.29 (hh3cIfCurrentFlowValue)
N/A
Counter64
Recommended action
1.When CurrentInputBroadcastRate BaseInputBroadcastRate+InputBroadcastChangeThreshold, identify whether the broadcast traffic increases normally. If not, identify whether loops exist in the link.
Basic information
OID
Event
Severity
Default status
The rapid change of inbound broadcast traffic on an interface restores
Recovery
Warning
ON
This notification is generated if the inbound broadcast traffic of an interface rapidly changes to drop below the threshold (CurrentInputBroadcastRateBaseInputBroadcastRate- InputBroadcastChangeThresholdd) within the specified time.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
N/A
Counter64
N/A
Counter64
Recommended action
hh3cIfFlowControlDLAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.63
The port does not forward packets but receives pause frames, or the port sends pause frames but does not receive packets
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.64 (hh3cIfFlowControlDLAlarmResume)
ON
This notification is generated in either of the following conditions:
The port does not forward packets, but receives a large number of pause frames.
The port continuously sends a large number of pause frames, but does not receive packets.
System impact
An interface cannot forward packets.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
To resolve this issue, collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
The port does not forward packets or receive pause frames, or the port sends pause frames and receives packets
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the port sends pause frames and receives packets or the port does not forward packets or receive pause frames.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
hh3cIfOutputErrorAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.65
Some service data on the port is dropped
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.66 (hh3cIfOutputErrorAlarmResume)
ON
This notification is generated if the optical transceiver module or optical fiber fails.
System impact
Some service data on the port is dropped.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Card index.
N/A
Integer32
0-65535
Subcard index.
N/A
Integer32
0-65535
Recommended action
To resolve this issue:
1.Replace the transceiver module. Identify whether the alarm is cleared.
2.Replace the optical fiber. Identify whether the alarm is cleared.
3.Collect alarm information and configuration data, and then contact H3C Support.
Basic information
OID
Event
Severity
Default status
No service data is dropped on the port.
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the optical transceiver module or optical fiber recovers and the service data on the port restores.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Card index.
N/A
Integer32
0-65535
Subcard index.
N/A
Integer32
0-65535
Recommended action
hh3cIfCableSnrAbnormal
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.67
The network cable quality is poor or signal interference occurs
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.68 (hh3cIfCableSnrNormal)
ON
This notification is generated when a multiGE copper port operates at 2.5 Gbps or higher and the network cable quality is poor or signal interference occurs.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
1.Replace the current cable with a higher-quality cable, for example, category 6A cable or shielded cable.
2.Execute the speed { 100 | 1000 } or auto speed { 100 | 1000 } command to set a lower speed for the multiGE interface.
Basic information
OID
Event
Severity
Default status
The network cable quality is good and no signal interference occurs
Recovery
Warning
N/A (N/A)
ON
This notification is generated when a multiGE copper port operates at 2.5 Gbps or higher, the network cable quality is good, and no signal interference occurs.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
hh3cIfCableSnrDetectNotSupport
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.69
A multiGE interface in up state goes down
Informational
Warning
N/A (N/A)
ON
This notification is generated when the network cable quality cannot be detected and a multiGE interface in up state goes down.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
1.The network cable quality cannot be detected. Replace the network cable.
hh3cIfSfpNotSupportSingleFiber
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.70
A transceiver module inserted into an interface does not support single fiber communication
Informational
Warning
N/A (N/A)
ON
This notification is generated when a transceiver module inserted into an interface does not support single fiber communication.
System impact
The single fiber communication function cannot be used on the interface because of the transceiver module inserted into the interface.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
To resolve this issue, replace the transceiver module with a transceiver module that supports single fiber communication.
hh3cIfLRMStateAbnormal
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.71
The interface does not support LRM transceiver modules
Informational
Warning
N/A (N/A)
ON
This notification is generated when the transceiver module inserted into an interface does not support LRM transceiver modules.
System impact
The transceiver module is not available, and the service of the interface is interrupted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
1.Execute the display transceiver command to view the type of the transceiver module installed in the interface.
2.Replace the transceiver module with a non-LRM transceiver module.
hh3cIfSfpWorkOnlyNonNego
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.72
A GE transceiver module installed in an XGE interface can operate only at non-autonegotiated 1000 Mbps
Informational
Warning
N/A (N/A)
ON
This notification is generated when a GE transceiver module installed in an XGE interface can operate only at non-autonegotiated 1000 Mbps and the interconnect interface is manually configured to operate at 1000 Mbps.
System impact
After an XGE interface has a GE transceiver module installed, the autonegotiation function of the interface is unavailable.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
Recommended action
To resolve this issue, manually configure the interconnect interface to operate at 1000 Mbps.
hh3cIfPfcDeadLockAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.73
PFC deadlock might cause traffic interruption on the network
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.74 (hh3cIfPfcDeadLockResume)
ON
This notification is generated when PFC deadlock occurs.
System impact
Traffic interruption might occur on the network.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Recommended action
1.Execute the display priority-flow-control command to identify the PFC deadlock reasons on the network and optimize the network. If this issue persists on the network, proceed with step 2.
2.Execute the priority-flow-control deadlock cos cos-value interval interval command to adjust the PFC deadlock detection interval to meet the actual network requirements.
Basic information
OID
Event
Severity
Default status
PFC deadlock recovers, and traffic is forwarded
Recovery
Warning
N/A (N/A)
ON
This notification is generated when PFC deadlock recovers and traffic can be normally forwarded.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Recommended action
hh3cIfPfcTurnOffAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.75
The number of PFC deadlock times exceeds the threshold for automatically disabling PFC
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.76 (hh3cIfPfcTurnOffResume)
ON
This notification is generated when the number of PFC deadlock times within a detection period exceeds the threshold for automatically disabling PFC.
System impact
PFC is automatically disabled.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Recommended action
2.Execute the priority-flow-control deadlock cos cos-value interval interval command to adjust the PFC deadlock detection interval and execute the priority-flow-control deadlock threshold cos cos-value period period count count command to adjust the number of PFC deadlock times for automatically disabling PFC to meet the actual network requirements.
3.If the PFC deadlock has been removed from the network, first execute the undo priority-flow-control enable command to disable PFC and then execute the priority-flow-control enable command to enable PFC on the interface, so that PFC is applied again.
Basic information
OID
Event
Severity
Default status
The number of PFC deadlock times is lower than the threshold for automatically disabling PFC
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the number of PFC deadlock times within a detection period is lower than the threshold for automatically disabling PFC.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Recommended action
hh3cIfQueueAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.77
The usage of a queue on an interface exceeds the threshold configured on the interface
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.78 (hh3cIfQueueResume)
ON
This notification is generated when the usage of a queue on an interface exceeds the threshold configured on the interface.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
1.3.6.1.4.1.25506.2.40.30.0 (hh3cIfCurrentUsedRatio)
Current queue usage
N/A
Unsigned32
1.3.6.1.4.1.25506.2.40.31.0 (hh3cIfUsedRatioThershold)
Queue usage threshold
N/A
Unsigned32
Recommended action
hh3cIfQueueResume
Basic information
OID
Event
Severity
Default status
The usage of a queue on an interface drops below the threshold configured on the interface
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the usage of a queue on an interface drops below the threshold configured on the interface.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Current queue usage
N/A
Unsigned32
N/A
Unsigned32
Recommended action
hh3cIfQueueStatDiscardAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.79
The number of dropped packets, the number of dropped bytes, or the packet loss ratio of a port queue exceeds the alarm threshold
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.80 (hh3cIfQueueStatDiscardResume)
ON
This notification is generated when the number of dropped packets, the number of dropped bytes, or the packet loss ratio of a port queue exceeds the alarm threshold.
System impact
Packet loss occurs, and services on the interface might be impacted.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
1.3.6.1.4.1.25506.2.40.31.0 (hh3cIfDiscardType)
Packet loss type
N/A
INTEGER
discardstat(1), discardByte(2), discardrate(3)
1.3.6.1.4.1.25506.2.40.31.0 (hh3cIfDiscardThreshold)
Packet loss threshold
N/A
Counter64
Recommended action
Basic information
OID
Event
Severity
Default status
The number of dropped packets, the number of dropped bytes, or the packet loss ratio of a port queue drops below the alarm threshold
Recovery
Warning
N/A (N/A)
ON
This notification is generated when the number of dropped packets, the number of dropped bytes, or the packet loss ratio of a port queue drops below the alarm threshold.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Packet loss type
N/A
INTEGER
N/A
Counter64
Recommended action
hh3cIfQueueEgressCongestionAlarm
Basic information
OID
Event
Severity
Default status
1.3.6.1.4.1.25506.2.40.3.0.81
Congestion occurs in the outbound direction of an interface queue
Error
Warning
1.3.6.1.4.1.25506.2.40.3.0.82 (hh3cIfQueueEgressCongestionClear)
ON
This notification is generated when congestion occurs in the outbound direction of an interface queue.
System impact
Outgoing traffic of an interface might be lost.
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Recommended action
To resolve this issue, adjust the network to relieve the network congestion.
Basic information
OID
Event
Severity
Default status
Congestion in the outbound direction of an interface queue is removed
Recovery
Warning
N/A (N/A)
ON
This recovery notification is generated when congestion in the outbound direction of an interface queue is removed.
System impact
Status control
Object
OID (object name)
Index
Value range
Interface index.
ifIndex
Integer32
ifIndex
OCTET STRING
hh3cIfQueId
INTEGER
Recommended action