02-System Management Configuration Guide
HomeSupportSwitchesS6550X-HI SeriesConfigure & DeployConfiguration GuidesH3C S6550X-HI Configuration Guides-R1116Pxx-6W10002-System Management Configuration Guide
04-EAA configuration
04-EAA configuration 145.59 KB
Configuring EAA
About EAA
Embedded Automation Architecture (EAA) is a monitoring framework that enables you to self-define monitored events and actions to take in response to an event. It allows you to create monitor policies by using the CLI or Tcl scripts.
EAA framework
EAA framework includes a set of event sources, a set of event monitors, a real-time event manager (RTM), and a set of user-defined monitor policies, as shown in Figure 1.
Figure 1 EAA framework
Event sources
Event sources are software or hardware modules that trigger events (see Figure 1).
For example, the CLI module triggers an event when you enter a command. The Syslog module (the information center) triggers an event when it receives a log message.
Event monitors
EAA creates one event monitor to monitor the system for the event specified in each monitor policy. An event monitor notifies the RTM to run the monitor policy when the monitored event occurs.
RTM
RTM manages the creation, state machine, and execution of monitor policies.
EAA monitor policies
A monitor policy specifies the event to monitor and actions to take when the event occurs.
You can configure EAA monitor policies by using the CLI or Tcl.
A monitor policy contains the following elements:
·     One event.
·     A minimum of one action.
·     A minimum of one user role.
·     One running time setting.
For more information about these elements, see "Elements in a monitor policy."
Elements in an EAA monitor policy include event, action, user role, and runtime.
Event
Table 1 shows types of events that EAA can monitor.
Table 1 Monitored events
Event type
CLI
CLI event occurs in response to monitored operations performed at the CLI. For example, a command is entered, a question mark (?) is entered, or the Tab key is pressed to complete a command.
Syslog
Syslog event occurs when the information center receives the monitored log within a specific period.
The log that is generated by the EAA RTM does not trigger the monitor policy to run.
Process
Process event occurs in response to a state change of the monitored process (such as an exception, shutdown, start, or restart). Both manual and automatic state changes can cause the event to occur.
Hotplug
Hot-swapping event occurs when a card is inserted in or removed from the monitored slot.
Each interface event is associated with two user-defined thresholds: start and restart.
An interface event occurs when the monitored interface traffic statistic crosses the start threshold in the following situations:
·     The statistic crosses the start threshold for the first time.
·     The statistic crosses the start threshold each time after it crosses the restart threshold.
SNMP
Each SNMP event is associated with two user-defined thresholds: start and restart.
SNMP event occurs when the monitored MIB variable's value crosses the start threshold in the following situations:
·     The monitored variable's value crosses the start threshold for the first time.
·     The monitored variable's value crosses the start threshold each time after it crosses the restart threshold.
SNMP-Notification
SNMP-Notification event occurs when the monitored MIB variable's value in an SNMP notification matches the specified condition. For example, the broadcast traffic rate on an Ethernet interface reaches or exceeds 30%.
Track
Track event occurs when the state of the track entry changes from Positive to Negative or from Negative to Positive. If you specify multiple track entries for a policy, EAA triggers the policy only when the state of all the track entries changes from Positive (Negative) to Negative (Positive).
If you set a suppress time for a policy, the timer starts when the policy is triggered. The system does not process the messages that report the track entry state change from  Positive (Negative) to Negative (Positive) until the timer times out.
Action
You can create a series of order-dependent actions to take in response to the event specified in the monitor policy.
The following are available actions:
·     Executing a command.
·     Sending a log.
·     Enabling an active/standby switchover.
·     Executing a reboot without saving the running configuration.
User role
For EAA to execute an action in a monitor policy, you must assign the policy the user role that has access to the action-specific commands and resources. If EAA lacks access to an action-specific command or resource, EAA does not perform the action and all the subsequent actions.
For example, a monitor policy has four actions numbered from 1 to 4. The policy has user roles that are required for performing actions 1, 3, and 4. However, it does not have the user role required for performing action 2. When the policy is triggered, EAA executes only action 1.
For more information about user roles, see RBAC in Fundamentals Configuration Guide.
Runtime
The runtime limits the amount of time that the monitor policy runs its actions from the time it is triggered. This setting prevents a policy from running its actions permanently to occupy resources.
EAA environment variables
EAA environment variables decouple the configuration of action arguments from the monitor policy so you can modify a policy easily.
An EAA environment variable is defined as a <variable_name variable_value> pair and can be used in different policies. When you define an action, you can enter a variable name with a leading dollar sign ($variable_name). EAA will replace the variable name with the variable value when it performs the action.
To change the value for an action argument, modify the value specified in the variable pair instead of editing each affected monitor policy.
EAA environment variables include system-defined variables and user-defined variables.
System-defined variables
System-defined variables are provided by default, and they cannot be created, deleted, or modified by users. System-defined variable names start with an underscore (_) sign. The variable values are set automatically depending on the event setting in the policy that uses the variables.
System-defined variables include the following types:
·     Public variable—Available for any events.
·     Event-specific variable—Available only for the specific event type. For example, the CLI event-specific variable is _cmd. When an CLI event is triggered, the value of _cmd is the command line matching the monitor policy.
Table 2 shows all system-defined variables.
Table 2 System-defined EAA environment variables by event type
Event
Variable name and description
Any event
_event_id: Event ID
_event_type: Event type
_event_type_string: Event type description
_event_time: Time when the event occurs
_event_severity: Severity level of an event
CLI
_cmd: Commands that are matched
Syslog
_syslog_pattern: Log message content
Hotplug
_slot: 1
_ifname: Interface name
SNMP
_oid: OID of the MIB variable where an SNMP operation is performed
_oid_value: Value of the MIB variable
SNMP-Notification
_oid: OID that is included in the SNMP notification.
Process
_process_name: Process name
User-defined variables
You can use user-defined variables for all types of events.
User-defined variable names can contain digits, characters, and the underscore sign (_), except that the underscore sign cannot be the leading character.
Configuring a user-defined EAA environment variable
Configure user-defined EAA environment variables so that you can use them when creating EAA monitor policies.
2.     Configure a user-defined EAA environment variable.
For the system-defined variables, see Table 2.
Configuring a monitor policy
Make sure the actions in different policies do not conflict. Policy execution result will be unpredictable if policies that conflict in actions are running concurrently.
You can assign the same policy name to a CLI-defined policy and a Tcl-defined policy. However, you cannot assign the same name to policies that are the same type.
A monitor policy supports only one event and runtime. If you configure multiple events for a policy, the most recent one takes effect.
A monitor policy supports a maximum of 64 valid user roles. User roles added after this limit is reached do not take effect.
Configuring a monitor policy from the CLI
You can configure a series of actions to be executed in response to the event specified in a monitor policy. EAA executes the actions in ascending order of action IDs. When you add actions to a policy, you must make sure the execution order is correct. If two actions have the same ID, the most recent one takes effect.
2.     (Optional.) Set the size for the EAA-monitored log buffer.
By default, the EAA-monitored log buffer can store a maximum of 50000 logs.
3.     Create a CLI-defined policy and enter its view.
rtm cli-policy policy-name
4.     Configure an event for the policy. Choose one option as needed. If you configure multiple events, the most recently configured event takes effect.
¡     Configure a CLI event.
¡     Configure a hotplug event.
event hotplug [ insert | remove ] slot slot-number
¡     Configure an interface event. Choose one option as needed:
event interface monitor-interface-list monitor-obj monitor-obj start-op start-op start-val start-val restart-op restart-op restart-val restart-val [ interval interval ]
event interface all monitor-obj monitor-obj start-op start-op start-val start-val restart-op restart-op restart-val restart-val [ interval interval ] exclude exclude-interface-list
¡     Configure a process event.
¡     Configure an SNMP event.
¡     Configure an SNMP-Notification event.
¡     Configure a Syslog event.
event syslog priority { priority | all } msg msg occurs times period period
¡     Configure a track event.
By default, a monitor policy does not contain an event.
5.     Configure the actions to take when the event occurs.
¡     Configure a CLI action.
¡     Configure a reboot action.
action number reboot [ slot slot-number [ subslot subslot-number ] ]
¡     Configure an active/standby switchover action.
action number switchover
¡     Configure a logging action.
By default, a monitor policy does not contain any actions.
6.     (Optional.) Assign a user role to the policy.
user-role role-name
By default, a monitor policy contains user roles that its creator had at the time of policy creation.
An EAA policy cannot have both the security-audit user role and any other user roles. Any previously assigned user roles are automatically removed when you assign the security-audit user role to the policy. The previously assigned security-audit user role is automatically removed when you assign any other user roles to the policy.
7.     (Optional.) Configure the policy action runtime.
running-time time
The default policy action runtime is 20 seconds.
If you configure multiple action runtimes for a policy, the most recent one takes effect.
8.     Enable the policy.
commit
By default, CLI-defined policies are not enabled.
A CLI-defined policy can take effect only after you perform this step.
Configuring a monitor policy by using Tcl
A Tcl script contains two parts: Line 1 and the other lines.
·     Line 1
Line 1 defines the event, user roles, and policy action runtime. After you create and enable a Tcl monitor policy, the device immediately parses, delivers, and executes Line 1.
Line 1 must use the following format:
::comware::rtm::event_register event-type arg1 arg2 arg3user-role role-name1 | [ user-role role-name2 | [ ] ] [ running-time running-time ]
¡     The arg1 arg2 arg3 … arguments represent event matching rules. If an argument value contains spaces, use double quotation marks ("") to enclose the value. For example, "a b c."
¡     The configuration requirements for the event-type, user-role, and running-time arguments are the same as those for a CLI-defined monitor policy.
·     The other lines
From the second line, the Tcl script defines the actions to be executed when the monitor policy is triggered. You can use multiple lines to define multiple actions. The system executes these actions in sequence. The following actions are available:
¡     Standard Tcl commands.
¡     EAA-specific Tcl actions:
-     switchover ( ::comware::rtm::action switchover )
-     syslog (::comware::rtm::action syslog priority priority facility local-number msg msg-body). For more information about these arguments, see EAA commands in System Management Command Reference.
¡     Commands supported by the device.
To revise the Tcl script of a policy, you must suspend all monitor policies first, and then resume the policies after you finish revising the script. The system cannot execute a Tcl-defined policy if you edit its Tcl script without first suspending these policies.
1.     Download the Tcl script file to the device by using FTP or TFTP.
For more information about using FTP and TFTP, see Fundamentals Configuration Guide.
2.     Create and enable a Tcl monitor policy.
a.     Enter system view.
b.     Create a Tcl-defined policy and bind it to the Tcl script file.
By default, no Tcl policies exist.
Suspending monitor policies
This task suspends all CLI-defined and Tcl-defined monitor policies. If a policy is running when you perform this task, the system suspends the policy after it executes all the actions.
To restore the operation of the suspended policies, execute the undo rtm scheduler suspend command.
2.     Suspend monitor policies.
Verifying and maintaining EAA
·     Display EAA monitor policies.
·     Display user-defined EAA environment variables.
To display the running configuration of a CLI-defined monitor policy, execute the following command in CLI-defined monitor policy view:
display this
EAA configuration examples
Example: Configuring a CLI event monitor policy by using Tcl
As shown in Figure 2, use Tcl to create a monitor policy on the Device. This policy must meet the following requirements:
·     EAA sends the log message "rtm_tcl_test is running" when a command that contains the display this string is entered.
·     The system executes the command only after it executes the policy successfully.
Figure 2 Network diagram
# Edit a Tcl script file (rtm_tcl_test.tcl, in this example) for EAA to send the message "rtm_tcl_test is running" when a command that contains the display this string is executed.
::comware::rtm::event_register cli sync mode execute pattern display this user-role network-admin
::comware::rtm::action syslog priority 1 facility local4 msg rtm_tcl_test is running
# Download the Tcl script file from the TFTP server at 1.2.1.1.
<Sysname> tftp 1.2.1.1 get rtm_tcl_test.tcl
# Create Tcl-defined policy test and bind it to the Tcl script file.
[Sysname] rtm tcl-policy test rtm_tcl_test.tcl
[Sysname] quit
# Display information about the policy.
Total number: 1
Type  Event      TimeRegistered       PolicyName
TCL   CLI        May 02 14:54:50 2019 test
# Enable the information center to output log messages to the current monitoring terminal.
<Sysname> terminal monitor
[Sysname] info-center enable
# Execute the display this command. Verify that the system displays the rtm_tcl_test is running message and a message that the policy is being successfully executed.
[Sysname] display this
return
<Sysname>%Jun  4 15:02:30:354 2019 Sysname RTM/1/RTM_ACTION: rtm_tcl_test is running
%Jun  4 15:02:30:382 2019 Sysname RTM/6/RTM_POLICY: TCL policy test is running successfully.
Example: Configuring a CLI event monitor policy from the CLI
Configure a policy from the CLI to monitor the event that occurs when a question mark (?) is entered at the command line that contains letters and digits.
When the event occurs, the system executes the command, sends the log message "hello world" to the information center, and creates a local device management user named user1.
# Create CLI-defined policy test and enter its view.
[Sysname] rtm cli-policy test
# Add a CLI event that occurs when a question mark (?) is entered at any command line that contains letters and digits.
[Sysname-rtm-test] event cli async mode help pattern [a-zA-Z0-9]
# Add an action that sends the message "hello world" with a priority of 4 from the logging facility local3 when the event occurs.
[Sysname-rtm-test] action 0 syslog priority 4 facility local3 msg “hello world”
# Add an action that enters system view when the event occurs.
[Sysname-rtm-test] action 2 cli system-view
# Add an action that create a local device management user named user1.
[Sysname-rtm-test] action 3 cli local-user user1 class manage
# Set the policy action runtime to 3000 seconds.
[Sysname-rtm-test] running-time 3000
# Specify the network-admin user role for executing the policy.
# Enable the policy.
[Sysname-rtm-test] commit
[Sysname-rtm-test] display rtm policy registered
Total number: 1
CLI   CLI        Aug 29 14:56:50 2019 test
[Sysname-rtm-test] return
[Sysname] quit
# Enter a question mark (?) at a command line that contains a letter d. Verify that the system displays the "hello world" message and a policy successfully executed message on the terminal screen.
<Sysname> d?
  debugging
  delete
  diagnostic-logfile
  dir
  display
<Sysname>d%Aug  29 14:57:20:218 2019 Sysname RTM/4/RTM_ACTION: "hello world"
%Aug  29 14:58:11:170 2019 Sysname RTM/6/RTM_POLICY: CLI policy test is running successfully.
Example: Configuring a track event monitor policy from the CLI
As shown in Figure 3, Device A has established BGP sessions with Device D and Device E. Traffic from Device D and Device E to the Internet is forwarded through Device A.
Configure a CLI-defined EAA monitor policy on Device A to disconnect the sessions with Device D and Device E when Twenty-FiveGigE 1/0/1 connected to Device C is down. In this way, traffic from Device D and Device E to the Internet can be forwarded through Device B.
Figure 3 Network diagram
# Display BGP peer information for Device A.
<DeviceA> display bgp peer ipv4
 BGP local router ID: 1.1.1.1
 Local AS number: 100
 Total number of peers: 3                  Peers in established state: 3
  * - Dynamically created peer
  10.2.1.2                200       13       16    0       0 00:16:12 Established
  10.3.1.2                300       13       16    0       0 00:10:34 Established
  10.3.2.2                300       13       16    0       0 00:10:38 Established
# Create track entry 1 and associate it with the link state of Twenty-FiveGigE 1/0/1.
<Device A> system-view
[Device A] track 1 interface twenty-fivegige 1/0/1
# Configure a CLI-defined EAA monitor policy so that the system automatically disables session establishment with Device D and Device E when Twenty-FiveGigE 1/0/1 is down.
[Device A] rtm cli-policy test
[Device A-rtm-test] event track 1 state negative
[Device A-rtm-test] action 0 cli system-view
[Device A-rtm-test] action 1 cli bgp 100
[Device A-rtm-test] action 2 cli peer 10.3.1.2 ignore
[Device A-rtm-test] action 3 cli peer 10.3.2.2 ignore
[Device A-rtm-test] user-role network-admin
[Device A-rtm-test] commit
[Device A-rtm-test] quit
# Shut down Twenty-FiveGigE 1/0/1.
[Device A] interface twenty-fivegige 1/0/1
[Device A-Twenty-FiveGigE1/0/1] shutdown
# Execute the display bgp peer ipv4 command on Device A to verify that no BGP peer is in established state.
Example: Configuring a CLI event monitor policy with EAA environment variables from the CLI
Define an environment variable to match the IP address 1.1.1.1.
Configure a policy from the CLI to monitor the event that occurs when a command line that contains loopback0 is executed. In the policy, use the environment variable for IP address assignment.
When the event occurs, the system performs the following tasks:
·     Creates the Loopback 0 interface.
·     Assigns 1.1.1.1/24 to the interface.
·     Sends the matching command line to the information center.
# Configure an EAA environment variable for IP address assignment. The variable name is loopback0IP, and the variable value is 1.1.1.1.
[Sysname] rtm environment loopback0IP 1.1.1.1
# Create the CLI-defined policy test and enter its view.
# Add a CLI event that occurs when a command line that contains loopback0 is executed.
[Sysname-rtm-test] event cli async mode execute pattern loopback0
[Sysname-rtm-test] action 0 cli system-view
# Add an action that creates the interface Loopback 0 and enters loopback interface view.
[Sysname-rtm-test] action 1 cli interface loopback 0
# Add an action that assigns the IP address 1.1.1.1 to Loopback 0. The loopback0IP variable is used in the action for IP address assignment.
[Sysname-rtm-test] action 2 cli ip address $loopback0IP 24
# Add an action that sends the matching loopback0 command with a priority of 0 from the logging facility local7 when the event occurs.
[Sysname-rtm-test] action 3 syslog priority 0 facility local7 msg $_cmd
<Sysname>
<Sysname> terminal log level debugging
# Execute the loopback0 command. Verify that the system displays the loopback0 message and a policy successfully executed message on the terminal screen.
[Sysname] interface loopback0
<Sysname>
%Jan  3 09:46:10:592 2019 Sysname RTM/7/RTM_ACTION: interface loopback0
%Jan  3 09:46:10:613 2019 Sysname RTM/6/RTM_POLICY: CLI policy test is running successfully.
# Verify that Loopback 0 has been created and assigned the IP address 1.1.1.1.
<Sysname> display interface loopback brief
Protocol: (s) - spoofing
Interface            Link Protocol Primary IP         Description
Loop0                UP   UP(s)    1.1.1.1
<Sysname>