H3C PS-2202-11L Power Supply Manual-5W100
HomeSupportServersPower SupplyInstall & UpgradePower Supply ManualsH3C PS-2202-11L Power Supply Manual-5W100
Table of Contents
Related Documents
01-Text
01-Text 214.63 KB
1 About the PS-2202-11L power supply
IMPORTANT
IMPORTANT:
·     The information in this document might differ from your product if it contains custom configuration options or features.
·     The figures in this document are for illustration only.
·     For the servers supported by the PS-2202-11L power supply, contact H3C Support.
The PS-2202-11L power supply supports AC input, high-voltage DC input, and DC output, and provides a maximum rated output of 2000 W.
Table1-1 PS-2202-11L power supply description
Item
Product code
UN-PS-2202-11L
Detailed description
2000W AC & 240V HVDC Power Supply (LT-R1-Platinum-Light Load and High Efficiency)(CTO&BTO)
Sales code
0231AHRU
Lowest-level code
0213A0A9
Figure1-1 PS-2202-11L power supply
Figure1-2 Front panel
(1) Power supply LED
(2) Latch
(3) Power receptacle
(4) Handle
2 Key features
Protection
The power supply provides protection against input overcurrent, input undervoltage, output overvoltage, output limit, output short circuit, and overtemperature conditions.
Redundancy
Multiple power supplies can be connected in parallel to achieve N+1 or N+N redundancy and load balancing.
Hot swapping
You can install or remove a power supply when the device is operating.
Tool free replacement
You can replace a power supply without using the tools.
3 Technical specifications
Table3-1 Technical specifications
Item
Specifications
Model
PS-2202-11L
Rated input voltage range
·     100 VAC to 120 VAC @ 1000 W
·     200 VAC to 240 VAC @ 2000 W
·     192 VDC to 288 VDC (240 HVDC power source) @ 2000 W
Rated input current range
·     12 A @ 100 VAC to 120 VAC
·     12 A @ 200 VAC to 240 VAC
·     10 A Max @ 240 VDC
Maximum rated heat dissipation
·     3892 BTU/hr @ 100 VAC
·     7636 BTU/hr @ 220 VAC
·     7593 BTU/hr @ 240 VAC
·     7596 BTU/hr @ 240 VDC
·     7552 BTU/hr @ 270 VDC
Maximum rated output power
2000 W
Frequency
50/60Hz @ 100 VAC to 240 VAC
Efficiency at 50% load
80 Plus Platinum
Temperature
·     Operating: 0°C to 55°C (32°F to 131°F)
·     Storage: –40°C to +85°C (–40°F to +185°F)
Operating humidity
5% to 90%
Maximum altitude
5000 m (16404.20 ft)
Redundancy
Yes
Cold backup
Yes
4 LEDs
Table4-1 Power supply LED description
LED status
Steady green
The power supply is operating correctly.
Flashing green (1 Hz)
Power is being input correctly but the system is not powered on.
Flashing green (0.33 Hz)
The power supply is in standby state and does not output power.
Flashing green (2 Hz)
The power supply is updating its firmware.
Steady amber
·     The power supply is faulty.
·     The power supply does not have power input, but the other power supply has correct power input.
Flashing amber (1 Hz)
An alarm has occurred on the power supply.
Off
No power supplies have power input, which can be caused by an incorrect power cord connection or power source shutdown.
5 Installing and removing the power supply
For information about installing and removing the power supply, see the user guide for the device.
