09-Security Configuration Examples
HomeSupportSwitchesS7500E SeriesConfigure & DeployConfiguration ExamplesH3C S7500E Switch Series Configuration Examples-R7585P05-6W10009-Security Configuration Examples
02-H3C_Port_Security_Configuration_Examples
02-H3C_Port_Security_Configuration_Examples 453.23 KB
H3C Port Security Configuration Examples
Software version: Release 7585P05
Document version: 6W100-20200330
Copyright © 2020 New H3C Technologies Co., Ltd. All rights reserved.
Introduction
This document provides port security configuration examples.
This document assumes that you have basic knowledge of port security.
General restrictions and guidelines
When you configure port security, follow these restrictions and guidelines:
·          Disable global 802.1X and MAC authentications before you enable port security on a port.
·          Port security automatically modifies the following 802.1X or MAC authentication settings for different security modes:
¡  The status of 802.1X and MAC authentication.
¡  The 802.1X access control method.
¡  The 802.1X port authorization state.
·          You cannot disable port security when online users are present.
·          Port security modes are mutually exclusive with link aggregation and service loopback group.
·          The maximum number of users a port supports equals the smaller value from the following values:
¡  The maximum number of secure MAC addresses that port security allows.
¡  The maximum number of concurrent users the authentication mode in use allows.
For example, if 802.1X allows more concurrent users than port security's limit on the number of MAC addresses on the port in userLoginSecureExt mode, port security's limit takes effect.
·          To change the security mode of a port security-enabled port, you must use the undo port-security port-mode command to set the port in noRestrictions mode first.
Example: Configuring autoLearn mode
As shown in Figure 1, configure port security mode autoLearn on Ten-GigabitEthernet 1/0/1 to meet the following requirements:
·          The device accepts a maximum of 64 users to log in through the port without authentication.
·          After the number of users reaches 64, the port denies any new users to access the Internet.
Figure 1 Network diagram
Analysis
To meet the network requirements, you must perform the following tasks:
·          Configure the autoLearn mode on the port through which the users access the device. The access port is Ten-GigabitEthernet 1/0/1 in this example.
·          Configure an aging timer for the secure MAC addresses, so the device can update its secure MAC address table.
·          Configure Ten-GigabitEthernet 1/0/1 to shut down temporarily for 30 seconds when it receives illegal frames. The device can deny any new users to access the Internet after the number of online users reaches 64.
Before you enable the autoLearn mode, set the maximum number of secure MAC addresses that port security allows on the port (by using the port-security max-mac-count command). You cannot change the setting when the port is operating in autoLearn mode.
Procedures
# Enable port security.
[Device] port-security enable
# Set the secure MAC aging timer to 30 minutes.
[Device] port-security timer autolearn aging 30
# Set port security's limit on the number of secure MAC addresses to 64 on Ten-GigabitEthernet 1/0/1.
[Device-Ten-GigabitEthernet1/0/1] port-security max-mac-count 64
# Set the port security mode to autoLearn.
[Device-Ten-GigabitEthernet1/0/1] port-security port-mode autolearn
# Specify the intrusion protection action as disableport-temporarily.
[Device-Ten-GigabitEthernet1/0/1] port-security intrusion-mode disableport-temporarily
# Configure the port to be silent for 30 seconds after the intrusion protection feature is triggered.
[Device] port-security timer disableport 30
# Verify that port security is correctly configured.
[Device] display port-security interface ten-gigabitethernet 1/0/1
Global port security parameters:
   Port security          : Enabled
   AutoLearn aging time   : 30 min
   Disableport timeout    : 30 s
   Blockmac timeout       : 180 s
   MAC move               : Denied
   Authorization fail     : Online
   NAS-ID profile         : Not configured
   Dot1x-failure trap     : Disabled
   Dot1x-logon trap       : Disabled
   Dot1x-logoff trap      : Disabled
   Intrusion trap         : Disabled
   Address-learned trap   : Disabled
   Mac-auth-failure trap  : Disabled
   Mac-auth-logon trap    : Disabled
   Mac-auth-logoff trap   : Disabled
   Open authentication    : Disabled
   OUI value list         :
 Ten-GigabitEthernet1/0/1 is link-up
   Port mode                      : autoLearn
   NeedToKnow mode                : Disabled
   Intrusion protection mode      : DisablePortTemporarily
   Security MAC address attribute
       Learning mode              : Sticky
       Aging type                 : Periodical
   Max secure MAC addresses       : 64
   Current secure MAC addresses   : 5
   Authorization                  : Permitted
   Free VLANs                     : Not configured
   MAC-move VLAN check bypass     : Disabled
The port allows for MAC address learning, and you can view the number of learned MAC addresses in the Current secure MAC addresses field.
# Display information about the learned MAC addresses.
[Device-Ten-GigabitEthernet1/0/1] display this
 port link-mode bridge
 port-security mac-address security sticky 00e0-fc00-5920 vlan 1
 port-security mac-address security sticky 00e0-fc00-592a vlan 1
 port-security mac-address security sticky 00e0-fc00-592b vlan 1
 port-security mac-address security sticky 00e0-fc00-592c vlan 1
 port-security mac-address security sticky 00e0-fc00-592d vlan 1
# Verify that the port security mode changes to secure after the number of MAC addresses learned by the port reaches 64.
# Verify that the port is disabled after it receives a frame with an unknown MAC address.
[Device] display interface ten-gigabitethernet 1/0/1
# Verify that the interface is re-enabled after 30 seconds.
# Delete several secure MAC addresses.
[Device-Ten-GigabitEthernet1/0/1] undo port-security mac-address security sticky 00e0-fc00-5920 vlan 1
[Device-Ten-GigabitEthernet1/0/1] undo port-security mac-address security sticky 00e0-fc00-592a vlan 1
# Verify that the port security mode changes to autoLearn and the port can learn MAC addresses again. (Details not shown.)
Configuration files
Example: Configuring userLoginWithOUI mode
As shown in Figure 2:
·          Users use the 802.1X client on the host to initiate 802.1X authentication.
·          The device uses the RADIUS server to perform authentication, authorization, and accounting for all users in ISP domain sun.
·          IMC is the RADIUS server.
·          The device and the server use the shared key expert for secure RADIUS communication.
Configure port security mode userLoginWithOUI on the device to meet the following requirements:
·          Permit only one 802.1X user to pass authentication to access the Internet.
·          Permit the printer to access the Internet.
·          Discard all illegal frames without disabling the port security-enabled port.
Figure 2 Network diagram
Analysis
·          Configure the userLoginWithOUI mode on the port through which the users access the device. The access port is Ten-GigabitEthernet 1/0/1 in this example.
·          Add the printer's OUI to the port security module of the device, so the device can permit the printer to access the Internet in userLoginWithOUI mode. To match the OUIs of different printer vendors, add multiple OUIs to the device.
·          Configure the blockmac intrusion protection on Ten-GigabitEthernet 1/0/1, so the device adds the source MAC addresses of illegal frames to the blocked MAC address list. The device discards all frames sourced from the blocked MAC addresses.
Procedures
Configuring the RADIUS server
In this example, the RADIUS server runs IMC PLAT 7.0 (E0201) and IMC UAM 7.0 (E0201).
1.        Add the device to IMC as an access device:
a.    Click the User tab.
b.    From the navigation tree, select User Access Policy > Access Device Management > Access Device.
c.    Click Add.
The Add Access Device page appears.
d.    In the Access Configuration area, configure the following parameters:
-      Enter 1812 in the Authentication Port field, and enter 1813 in the Accounting Port field.
-      Select LAN Access Service from the Service Type list.
-      Select HP(Comware) from the Access Device Type list.
-      Enter expert in the Shared Key and Confirm Shared Key field.
-      Use the default values for other parameters.
e.    In the Device List area, click Select or Add Manually to add the device at 192.168.0.34 as an access device.
The IP address of the access device specified here must be the same as the source IP address of the RADIUS packets sent from the device. The source IP address is chosen in the following order on the device:
-      IP address specified by the nas-ip command.
-      IP address specified by the radius nas-ip command.
-      IP address of the outbound interface (the default).
f.     Click OK.
Figure 3 Adding the device as an access device
2.        Add an access policy:
b.    From the navigation tree, select User Access Policy > Access Policy.
c.    Click Add.
d.    On the page that appears, configure the following parameters, as shown in Figure 4:
-      Enter 802.1X-auth in the Access Policy Name field.
Figure 4 Adding an access policy
e.    Click OK.
3.        Add an access service:
b.    From the navigation tree, select User Access Policy > Access Service.
c.    Click Add.
d.    On the page that appears, configure the following parameters, as shown in Figure 5:
-      Enter 802.1X-auth in the Service Name field.
-      Select 802.1X-auth from the Default Access Policy list.
Figure 5 Adding an access service
e.    Click OK.
4.        Add an access user:
b.    From the navigation tree, select Access User Management > All Access Users.
The access user list appears.
c.    Click Add.
d.    On the Add Access User page, configure the following parameters, as shown in Figure 6:
-      Click Select or Add User to associate the user with IMC Platform user hello.
-      Enter 802.1X in the Account Name field.
-      Enter 802.1X in the Password and Confirm Password fields.
-      Configure other parameters in the Access Information area as needed.
-      Select 802.1X-auth from the Access Service list.
Figure 6 Adding an access user account
e.    Click OK.
Configuring the device
The following steps have AAA RADIUS commands. For more information about the AAA RADIUS commands, see AAA commands in the security command reference for the device.
1.        Assign an IP address to each interface, as shown in Figure 2. Make sure the host, printer, device, and RADIUS server can reach each other. (Details not shown.)
2.        Configure the RADIUS scheme:
# Create RADIUS scheme radsun.
[Device] radius scheme radsun
New RADIUS scheme.
# Specify the primary RADIUS authentication server at 192.168.0.38.
[Device-radius-radsun] primary authentication 192.168.0.38
# Specify the primary RADIUS accounting server at 192.168.0.38.
[Device-radius-radsun] primary accounting 192.168.0.38
# Set the authentication shared key to expert in plain text for secure communication between the device and the RADIUS server.
[Device-radius-radsun] key authentication simple expert
# Set the accounting shared key to expert in plain text for secure communication between the device and the RADIUS server.
[Device-radius-radsun] key accounting simple expert
# Set the response timeout time of the RADIUS server to 5 seconds.
[Device-radius-radsun] timer response-timeout 5
# Set the maximum number of RADIUS packet retransmission attempts to 5.
[Device-radius-radsun] retry 5
# Set the real-time accounting interval to 15 minutes.
[Device-radius-radsun] timer realtime-accounting 15
# Exclude domain names from the usernames sent to the RADIUS server.
[Device-radius-radsun] user-name-format without-domain
[Device-radius-radsun] quit
# Create ISP domain sun and enter ISP domain view.
[Device] domain sun
# Configure ISP domain sun to use RADIUS scheme radsun for authentication, authorization, and accounting of all LAN users.
[Device-isp-sun] authentication lan-access radius-scheme radsun
[Device-isp-sun] authorization lan-access radius-scheme radsun
[Device-isp-sun] accounting lan-access radius-scheme radsun
[Device-isp-sun] quit
# Configure domain sun as the default domain.
[Device] domain default enable sun
3.        Set the 802.1X authentication method to CHAP. By default, the authentication method for 802.1X is CHAP.
[Device] dot1x authentication-method chap
4.        Configure port security:
# Add five OUI values.
[Device] port-security oui index 1 mac-address 1234-0100-1111
[Device] port-security oui index 2 mac-address 1234-0200-1111
[Device] port-security oui index 3 mac-address 1234-0300-1111
[Device] port-security oui index 4 mac-address 1234-0400-1111
[Device] port-security oui index 5 mac-address 1234-0500-1111
# Set the port security mode to userLoginWithOUI.
[Device-Ten-GigabitEthernet1/0/1] port-security port-mode userlogin-withoui
# Configure port Ten-GigabitEthernet 1/0/1 to perform the blockmac intrusion protection action.
[Device-Ten-GigabitEthernet1/0/1] port-security intrusion-mode blockmac
# Display RADIUS scheme radsun.
[Device] display radius scheme radsun
RADIUS scheme name: radsun
  Index: 0
  Primary authentication server:
    IP   : 192.168.0.38                             Port: 1812
    VPN  : Not configured
    State: Active
    Test profile: Not configured
    Weight: 0
  Primary accounting server:
    IP   : 192.168.0.38                             Port: 1813
    State: Active
    Weight: 0
  Accounting-On function                     : Disabled
    extended function                        : Disabled
    retransmission times                     : 50
    retransmission interval(seconds)         : 3
  Timeout Interval(seconds)                  : 5
  Retransmission Times                       : 5
  Retransmission Times for Accounting Update : 5
  Server Quiet Period(minutes)               : 5
  Realtime Accounting Interval(seconds)      : 900
  Stop-accounting packets buffering          : Enabled
    Retransmission times                     : 500
  NAS IP Address                             : Not configured
  User Name Format                           : without-domain
  Data flow unit                             : Byte
  Packet unit                                : One
  Attribute 15 check-mode                    : Strict
  Attribute 25                               : Standard
  Attribute Remanent-Volume unit             : Kilo
  server-load-sharing                        : Disabled
  Attribute 31 MAC format                    : HH-HH-HH-HH-HH-HH
  Stop-accounting packets send-force         : Disabled
  Reauthentication server selection          : Inherit
# Display port security configuration on Ten-GigabitEthernet 1/0/1.
   AutoLearn aging time   : 0 min
   Disableport timeout    : 20 s
   MAC move               : Denied
   OUI value list         :
       Index :  1       Value : 123401
       Index :  2       Value : 123402
       Index :  3       Value : 123403
       Index :  4       Value : 123404
       Index :  5       Value : 123405
   Port mode                      : userLoginWithOUI
   Intrusion protection mode      : BlockMacAddress
   Max secure MAC addresses       : Not configured
   Current secure MAC addresses   : 0
After an 802.1X user comes online, the number of secure MAC addresses saved by the port is 1.
# Display 802.1X information.
[Device] display dot1x interface ten-gigabitethernet 1/0/1
# Verify that Ten-GigabitEthernet 1/0/1 allows a user whose MAC address has an OUI from the specified OUIs to pass authentication.
[Device] display mac-address interface ten-gigabitethernet 1/0/1
MAC Address      VLAN ID     State            Port/NickName            Aging
1234-0300-0011  1            Learned          XGE1/0/1                 Y
Configuration files
 port-security oui index 1 mac-address 1234-0100-0000
 port-security oui index 2 mac-address 1234-0200-0000
 port-security oui index 3 mac-address 1234-0300-0000
 port-security oui index 4 mac-address 1234-0400-0000
 port-security oui index 5 mac-address 1234-0500-0000
 key authentication cipher $c$3$s9TAYm34R8sS5k/Cylg2sDm69ZRupMvGJg==
 key accounting cipher $c$3$UaUPGk8AfZAQLHFlbKNcEoM2HXGiuWowBQ==
 retry 5
domain sun
Example: Configuring macAddressElseUserLoginSecure mode
As shown in Figure 7, the device uses the RADIUS server to perform authentication, authorization, and accounting for all users in domain sun.
Configure port security mode macAddressElseUserLoginSecure on the device to meet the following requirements:
·          Allow only one 802.1X user to pass authentication, and allow multiple MAC authentication users to pass authentication.
·          Perform MAC authentication first for an 802.1X user, and then 802.1X authentication if the user fails MAC authentication.
·          Use shared user account with username aaa and password 123456 for MAC authentication users.
·          Allow a maximum of 64 authenticated users.
·          Prevent frames from being sent to unknown MAC addresses.
Figure 7 Network diagram
Analysis
·          Configure the macAddressElseUserLoginSecure mode on the port through which the users access the device. The access port is Ten-GigabitEthernet 1/0/1 in this example.
·          Set the NTK mode to ntkonly, so the device will prevent frames from being sent to unknown MAC addresses. In this mode, the device permits only unicast frames that are destined for the authenticated MAC addresses.
Procedures
1.        Add the device to IMC as an access device in the same way the device is added to IMC in "Example: Configuring userLoginWithOUI mode."
2.        Add an access policy, an access service, and an access user for 802.1X authentication in the same way they are added in "Example: Configuring userLoginWithOUI mode."
3.        Add an access policy for MAC authentication:
c.    Click Add.
d.    On the page that appears, configure the following parameters, as shown in Figure 8:
-      Enter MAC-auth in the Access Policy Name field.
Figure 8 Adding an access policy
e.    Click OK.
4.        Add an access service for MAC authentication:
c.    Click Add.
d.    On the page that appears, configure the following parameters, as shown in Figure 9:
-      Enter MAC-auth in the Service Name field.
-      Select MAC-auth from the Default Access Policy list.
Figure 9 Adding an access service
e.    Click OK.
5.        Add an access user for MAC authentication:
c.    Click Add.
d.    On the Add Access User page, configure the following parameters, as shown in Figure 10:
-      Click Select or Add User to associate the user with IMC Platform user hello2.
-      Enter aaa in the Account Name field.
-      Enter 123456 in the Password and Confirm Password fields.
-      Select MAC-auth from the Access Service list.
Figure 10 Adding an access user account
e.    Click OK.
1.        Assign an IP address to each interface, as shown in Figure 7. Make sure the hosts, device, and RADIUS server can reach each other. (Details not shown.)
New RADIUS scheme.
[Device] domain sun
# Specify ISP domain sun as the default domain.
3.        Configure MAC authentication:
# Configure a shared account for MAC authentication users, and set the username to aaa and password to plaintext string of 123456.
[Device] mac-authentication user-name-format fixed account aaa password simple 123456
# Specify domain sun as the global MAC authentication domain.
[Device] mac-authentication domain sun
4.        Set the 802.1X authentication method to CHAP. By default, the authentication method for 802.1X is CHAP.
5.        Configure port security:
# Set the port security mode to macAddressElseUserLoginSecure.
[Device-Ten-GigabitEthernet1/0/1] port-security port-mode mac-else-userlogin-secure
# Set the NTK mode of the port to ntkonly.
[Device-Ten-GigabitEthernet1/0/1] port-security ntk-mode ntkonly
   MAC move               : Denied
   OUI value list         :
   Port mode                      : macAddressElseUserLoginSecure
   NeedToKnow mode                : NeedToKnowOnly
   Intrusion protection mode      : NoAction
# Verify that port GigabitEthernet 1/0/1 allows multiple MAC authentication users to be authenticated.
[Device] display mac-authentication interface ten-gigabitethernet 1/0/1
   MAC authentication                  : Enabled
   Authentication method               : PAP
   Username format                     : Fixed account
           Username                    : aaa
           Password                    : ******
   Offline detect period               : 300 s
   Quiet period                        : 60 s
   Server timeout                      : 100 s
   Reauth period                       : 3600 s
   User aging period for critical VLAN : 1000 s
   User aging period for critical VSI  : 1000 s
   User aging period for guest VLAN    : 1000 s
   User aging period for guest VSI     : 1000 s
   Authentication domain               : sun
 Online MAC-auth wired user            : 3
 Silent MAC users:
          MAC address       VLAN ID  From port               Port index
   Carry User-IP                    : Disabled
   Authentication domain            : Not configured
   Auth-delay timer                 : Disabled
   Auth-delay period                : 60 s
   Periodic reauth                  : Disabled
   Re-auth server-unreachable       : Logoff
   Guest VLAN                       : Not configured
   Guest VLAN auth-period           : 30
   Critical VLAN                    : Not configured
   Critical voice VLAN              : Disabled
   Host mode                        : Single VLAN
   Offline detection                : Enabled
   Authentication order             : Default
   User aging                       : Enabled
   Server-recovery online-user-sync : Enabled
   Guest VSI                        : Not configured
   Guest VSI auth-period            : 30 s
   Critical VSI                     : Not configured
   Max online users                 : 4294967295
   Authentication attempts          : successful 0, failed 0
   Current online users             : 3
          MAC address       Auth state
          1234-0300-0011   authenticated
          1234-0300-0012   authenticated
          1234-0300-0013   authenticated
# Verify that Ten-GigabitEthernet 1/0/1 allows only one 802.1X user to be authenticated.
Global 802.1X parameters:
   802.1X authentication                : Enabled
   CHAP authentication                  : Enabled
   Max-tx period                        : 30 s
   Handshake period                     : 15 s
   Quiet timer                          : Disabled
       Quiet period                     : 60 s
   Supp timeout                         : 30 s
   Max auth requests                    : 2
   User aging period for Auth-Fail VLAN : 1000 s
   User aging period for Auth-Fail VSI  : 1000 s
   EAD assistant function               : Disabled
       EAD timeout                      : 30 min
   Domain delimiter                     : @
 Online 802.1X wired users              : 1
   Handshake                        : Enabled
   Handshake reply                  : Disabled
   Handshake security               : Disabled
   Offline detection                : Disabled
   Unicast trigger                  : Disabled
   Port role                        : Authenticator
   Authorization mode               : Auto
   Port access control              : MAC-based
   Multicast trigger                : Enabled
   Mandatory auth domain            : Not configured
   Auth-Fail VLAN                   : Not configured
   Add Guest VLAN delay             : Disabled
   User IP freezing                 : Disabled
   Reauth period                    : 0 s
   Send Packets Without Tag         : Disabled
   Max Attempts Fail Number         : 0
   Auth-Fail VSI                    : Not configured
   Add Guest VSI delay              : Disabled
   Auth-Fail EAPOL                  : Disabled
   Critical EAPOL                   : Disabled
   EAPOL packets: Tx 0, Rx 0
   Sent EAP Request/Identity packets : 0
        EAP Request/Challenge packets: 0
        EAP Success packets: 0
        EAP Failure packets: 0
   Received EAPOL Start packets : 0
            EAPOL LogOff packets: 0
            EAP Response/Identity packets : 0
            EAP Response/Challenge packets: 0
            Error packets: 0
   Online 802.1X users: 1
          0001-0000-0000      Authenticated
# Verify that frames with an unknown destination MAC address, multicast address, or broadcast address are discarded. (Details not shown.)
Configuration files
 mac-authentication user-name-format fixed account aaa password cipher $c$3$HAlQ
nyXOwZXTgiOBPd7+kSPClKm7JbZ1Rw==
 retry 5
domain sun
Related documentation
·          H3C S7500E Switch Series Security Configuration Guide-R758X
·          H3C S7500E Switch Series Security Command Reference-R758X