16-High Availability Command Reference
HomeSupportReference GuidesCommand ReferencesH3C SecPath Firewall Series Command References(V7)-6W40016-High Availability Command Reference
01-VRRP commands
01-VRRP commands 280.55 KB
VRRP commands
VRRP does not take effect on member ports of aggregation groups.
IPv4 VRRP commands
display vrrp
Use display vrrp to display the states of IPv4 VRRP groups.
display vrrp [ interface interface-type interface-number [ vrid virtual-router-id ] ] [ verbose ]
context-admin
context-operator
vrid virtual-router-id: Specifies an IPv4 VRRP group by its virtual router ID in the range of 1 to 255.
verbose: Displays detailed IPv4 VRRP group information. If you do not specify the verbose keyword, the command displays brief IPv4 VRRP group information.
If no interface or VRRP group is specified, this command displays the states of all IPv4 VRRP groups.
If only an interface is specified, this command displays the states of all IPv4 VRRP groups on the specified interface.
If both an interface and an IPv4 VRRP group are specified, this command displays the states of the specified IPv4 VRRP group on the specified interface.
# Display brief information about all IPv4 VRRP groups on the device when VRRP operates in standard mode.
<Sysname> display vrrp
 Running Mode      : Standard
 RBM control channel is established
   VRRP active group status: Master
   VRRP standby group status: Backup
 Interface          VRID  State        Running Adver   Auth     Virtual
                                       Pri     Timer   Type        IP
 GE1/0/1            1     Master       150     100     Simple   1.1.1.1
Table 1 Command output (in standard mode)
Running Mode
VRRP operating mode (standard mode).
The RBM control channel has been established.
This field is displayed only when VRRP is associated with RBM.
Running status of the device in the VRRP active group: Master or Backup.
Running status of the device in the VRRP standby group: Master or Backup.
Total number of VRRP groups.
Interface where the VRRP group is configured.
VRID
Virtual router ID (VRRP group number).
State of the router in the VRRP group:
·     Master—The router is the master in the VRRP group.
·     Backup—The router is the backup in the VRRP group.
·     Initialize—The router is in Initialize state.
·     Inactive—The router is in Inactive state, for example, when the router is not assigned a virtual IP address by using the vrrp vrid command.
Running Pri
Current priority of the router.
When a track entry is associated with a VRRP group on the router, the router's priority changes when the track entry's status changes.
Adver Timer
VRRP advertisement sending interval in centiseconds.
Auth Type
Authentication type:
·     None—No authentication.
·     Simple—Simple text authentication.
·     MD5—MD5 authentication.
Virtual IP
Virtual IP address of the VRRP group.
# Display detailed information about all IPv4 VRRP groups on the device when VRRP operates in standard mode.
<Sysname> display vrrp verbose
 Total number of virtual routers : 3
     VRID             : 1                    Adver Timer  : 100
     Admin Status     : Up                   State        : Master
     Config Pri       : 150                  Running Pri  : 150
     Preempt Mode     : Yes                  Delay Time   : 5
     Auth Type        : Simple               Key          : ******
     Virtual IP       : 1.1.1.1
     Virtual MAC      : 0000-5e00-0101
     Master IP        : 1.1.1.2
     VRID (group)     : 2 (Active)           Adver Timer  : 100
     Config Pri       : 100                  Running Pri  : 100
     Virtual IP       : 1.1.1.11
     Virtual MAC      : 0000-5e00-0102
     Master IP        : 1.1.1.2
     VRID  (group)    : 3  (Standby)         Adver Timer  : 100
     Admin Status     : Up                   State        : Backup
     Config Pri       : 80                   Running Pri  : 80
     Preempt Mode     : Yes                  Delay Time   : 0
     Become Master    : 2370ms left
     Auth Type        : --
     Master IP        : 1.1.1.12
Table 2 Command output (in standard mode)
Running Mode
VRID (group)
Virtual router ID.
The type of group (active or standby) associated with RBM is also displayed when VRRP is associated with RBM.
Adver Timer
Admin Status
Administrative status: Up or Down.
Config Pri
Configured priority of the router, which is configured by using the vrrp vrid priority command.
Running Pri
Preempt Mode
Preemptive mode:
·     Yes.
·     No.
Delay Time
Preemption delay in centiseconds.
Become Master
Time (in milliseconds) that a backup router has to wait before it becomes the master. This field is displayed only when the router is a backup. This field displays two hyphens (--) when VRRP is associated with RBM.
Auth Type
Key
Authentication key, which is not displayed if no authentication is required.
Virtual IP
Virtual MAC
Virtual MAC address of the VRRP group's virtual IP address, which is displayed when the router is the master.
Master IP
Primary IP address of the interface where the master resides.
VRRP Track Information
Track entry information. This field is displayed only after you configure the vrrp vrid track command.
Track Object
Track entry which is associated with the VRRP group.
Track entry state:
·     Negative.
·     Positive.
·     NotReady.
Pri Reduced
Value by which the priority decreases when the status of the associated track entry changes to the Negative state.
Switchover
Switchover mode. When the status of the associated track entry changes to the Negative state, the backup immediately becomes the master.
# Display brief information about all IPv4 VRRP groups on the device when VRRP operates in load balancing mode.
 Running Mode      : Load Balance
 Interface          VRID  State        Running Address             Active
                                       Pri
 GE1/0/1            1     Master       150     1.1.1.1             Local
 -----              VF 1  Active       255     000f-e2ff-0011      Local
Table 3 Command output (in load balancing mode)
Running Mode
VRRP operating mode (load balancing mode).
VRID
Virtual router ID (VRRP group number) or virtual forwarder (VF) ID.
·     For a VRRP group, this field indicates the state of the router in the VRRP group:
¡     Master—The router is the master in the VRRP group.
¡     Backup—The router is the backup in the VRRP group.
¡     Initialize—The router is in Initialize state.
¡     Inactive—The router is in Inactive state, for example, when the router is not assigned a virtual IP address by using the vrrp vrid command.
·     For a VF, this field indicates the state of the VF in the VRRP group:
¡     Active—The VF is created on the device.
¡     Listening—The VF is learned from another device.
¡     Initialize—The VF is in Initialize state.
Running Pri
·     For a VRRP group, this field indicates the running priority of the router. When a track entry is associated with a VRRP group on the router, the router's priority changes when the track entry's status changes.
·     For a VF, this field indicates the running priority of the VF. When a track entry is associated with a VF, the priority of the VF changes if the track entry's status changes.
Address
·     For a VRRP group, this field indicates the virtual IP address of the VRRP group.
·     For a VF, this field indicates the virtual MAC address of the VF.
Active
·     For a VRRP group, this field indicates the IP address of the interface where the master resides. If the current router is the master, this field displays local.
·     For a VF, this field indicates the IP address of the interface where the active virtual forwarder (AVF) resides. If the current VF is the AVF, this field displays local.
# Display detailed information about all IPv4 VRRP groups on the device when VRRP operates in load balancing mode.
     Auth Type      : None
     Virtual IP     : 10.1.1.1
                      10.1.1.2
                      10.1.1.3
     Member IP List : 10.1.1.10 (Local, Master)
                      10.1.1.20 (Backup)
   VRRP Track Information:
     Track Object   : 1                    State : Positive   Pri Reduced : 50
   Forwarder Information: 2 Forwarders 1 Active
     Config Weight  : 255
     Running Weight : 255
    Forwarder 01
     State          : Active
     Virtual MAC    : 000f-e2ff-0011 (Owner)
     Owner ID       : 0000-5e01-1101
     Priority       : 255
     Active         : local
    Forwarder 02
     State          : Listening
     Virtual MAC    : 000f-e2ff-0012 (Learnt)
     Owner ID       : 0000-5e01-1103
     Priority       : 127
     Active         : 10.1.1.20
   Forwarder Weight Track Information:
     Track Object   : 1          State : Positive   Weight Reduced : 250
     VRID           : 11                   Adver Timer  : 100
     Auth Type      : None
     Virtual IP     : 10.1.1.11
                    : 10.1.1.12
                    : 10.1.1.13
     Member IP List : 10.1.1.10 (Local, Backup)
                      10.1.1.15 (Master)
     Config Weight  : 255
    Forwarder 01
     State          : Active
     Virtual MAC    : 000f-e2ff-40b1 (Learnt)
     Priority       : 127
     Active         : 10.1.1.15
    Forwarder 02
     State          : Listening
     Virtual MAC    : 000f-e2ff-40b2 (Owner)
     Priority       : 255
     Active         : local
Table 4 Command output (in load balancing mode)
Running Mode
VRID
Adver Timer
Admin Status
Config Pri
Running Pri
Preempt Mode
Preemptive mode:
·     Yes.
·     No.
Delay Time
Become Master
Auth Type
Key
Virtual IP
Virtual IP address list of the VRRP group.
Member IP List
IP addresses of the member devices in the VRRP group:
·     Local—IP address of the local router.
·     Master—IP address of the master.
·     Backup—IP address of the backup.
Track entry which is associated with the VRRP group. This field is displayed only after you configure the vrrp vrid track command.
Track Object
Track entry to be monitored.
Track entry state:
·     Negative.
·     Positive.
·     NotReady.
Pri Reduced
Value by which the priority decreases when the status of the associated track entry changes to the Negative state. This field is displayed only after you configure the vrrp vrid track command.
Switchover
VF information: Two VFs exist, and one is the AVF.
Config Weight
Configured weight of the VF: 255.
Running Weight
Current weight of the VF.
When a track entry is associated with the VFs of a VRRP group, the VFs' weights change when the track entry's status changes.
Forwarder 01
Information about VF 01.
VF state:
·     Active—The VF is created on the device.
·     Listening—The VF is learned from another device.
·     Initialize—The VF is in Initialize state.
Virtual MAC
Virtual MAC address of the VF.
Owner ID
Real MAC address of the VF owner.
Priority
VF priority in the range of 1 to 255.
Active
IP address of the interface where the AVF resides. If the current VF is the AVF, this field displays local.
Forwarder Weight Track Configuration
VF weight Track configuration.
The field is displayed only after you configure the vrrp vrid track command.
Track Object
Track entry that is associated with the VFs.
Track entry state:
·     Negative.
·     Positive.
·     NotReady.
Weight Reduced
Value by which the weights of the VFs decrease when the state of the associated track entry changes to Negative.
Forwarder Switchover Track Information:
VF switchover Track configuration.
Member IP
IP address of a member device.
display vrrp statistics
Use display vrrp statistics to display statistics for IPv4 VRRP groups.
context-admin
context-operator
If no interface or VRRP group is specified, this command displays statistics for all IPv4 VRRP groups.
If only an interface is specified, this command displays statistics for all IPv4 VRRP groups on the specified interface.
If both an interface and an IPv4 VRRP group are specified, this command displays statistics for the specified IPv4 VRRP group on the specified interface.
# Display statistics for all IPv4 VRRP groups when VRRP operates in standard mode.
<Sysname> display vrrp statistics
 Interface               : GigabitEthernet1/0/1
 VRID                    : 1
 CheckSum Errors         : 0          Version Errors                : 0
 Invalid Pkts Rcvd  :      0          Unexpected Pkts Rcvd          : 0
 IP TTL Errors           : 0          Advertisement Interval Errors : 0
 Invalid Auth Type       : 0          Auth Failures                 : 0
 Packet Length Errors    : 0          Auth Type Mismatch            : 0
 Become Master           : 1          Address List Errors           : 0
 Adver Rcvd              : 0          Priority Zero Pkts Rcvd       : 0
 Adver Sent              : 807        Priority Zero Pkts Sent       : 0
 Global statistics
 CheckSum Errors         : 0
 Version Errors          : 0
 VRID Errors             : 0
# Display statistics for all IPv4 VRRP groups when VRRP operates in load balancing mode.
 VRID                    : 1
 Become Master           : 39         Address List Errors           : 0
 Become AVF              : 13         Packet Option Errors          : 0
 Adver Rcvd              : 2562       Priority Zero Pkts Rcvd       : 1
 Adver Sent              : 16373      Priority Zero Pkts Sent       : 49
 Request Rcvd            : 2          Reply Rcvd                    : 10
 Request Sent            : 12         Reply Sent                    : 2
 Release Rcvd            : 0          VF Priority Zero Pkts Rcvd    : 1
 Release Sent            : 0          VF Priority Zero Pkts Sent    : 11
 Redirect Timer Expires  : 1          Time-out Timer Expires        : 0
 Global statistics
 CheckSum Errors         : 0
 Version Errors          : 0
 VRID Errors             : 0
Table 5 Command output (in standard mode)
VRID
VRRP group number.
CheckSum Errors
Number of packets with checksum errors.
Version Errors
Number of packets with version errors.
Invalid Pkts Rcvd
Number of received packets of invalid packet types.
Number of received unexpected packets.
Number of packets with advertisement interval errors.
IP TTL Errors
Number of packets with TTL errors.
Auth Failures
Number of packets with authentication failures.
Invalid Auth Type
Number of packets with authentication failures because of invalid authentication types.
Auth Type Mismatch
Number of packets with authentication failures because of mismatching authentication types.
Number of packets with VRRP packet length errors.
Address List Errors
Number of packets with virtual IP address list errors.
Become Master
Number of times that the router has been elected as the master.
Number of received advertisements with the router priority of 0.
Adver Rcvd
Number of received advertisements.
Number of sent advertisements with the router priority of 0.
Adver Sent
Number of sent advertisements.
Global statistics
Global statistics for all VRRP groups.
CheckSum Errors
Total number of packets with checksum errors.
Version Errors
Total number of packets with version errors.
VRID Errors
Total number of packets with VRID errors.
Table 6 Command output (in load balancing mode)
VRID
VRRP group number.
CheckSum Errors
Version Errors
Invalid Pkts Rcvd
IP TTL Errors
Auth Failures
Invalid Auth Type
Auth Type Mismatch
Address List Errors
Become Master
Number of times that the redirect timer expired.
Become AVF
Number of times that the VF has been elected as the AVF.
Number of times that the time-out timer expired.
Adver Rcvd
Request Rcvd
Number of received requests.
Adver Sent
Request Sent
Number of sent requests.
Reply Rcvd
Number of received replies.
Release Rcvd
Number of received release packets.
Reply Sent
Number of sent replies.
Release Sent
Number of sent release packets.
Number of received advertisements with the VF priority of 0.
Number of sent advertisements with the VF priority of 0.
Number of packet option errors.
Global statistics
Global statistics for all IPv4 VRRP groups.
CheckSum Errors
Version Errors
VRID Errors
reset vrrp statistics
Use reset vrrp statistics to clear statistics for IPv4 VRRP groups.
context-admin
If no interface or VRRP group is specified, this command clears statistics for all IPv4 VRRP groups.
If only an interface is specified, this command clears statistics for all IPv4 VRRP groups on the specified interface.
If both an interface and an IPv4 VRRP group are specified, this command clears statistics for the specified IPv4 VRRP group on the specified interface.
# Clear statistics for all IPv4 VRRP groups on all interfaces.
<Sysname> reset vrrp statistics
snmp-agent trap enable vrrp
Use snmp-agent trap enable vrrp to enable SNMP notifications for VRRP.
Use undo snmp-agent trap enable vrrp to disable SNMP notifications for VRRP.
snmp-agent trap enable vrrp [ auth-failure | new-master ]
undo snmp-agent trap enable vrrp [ auth-failure | new-master ]
SNMP notifications for VRRP are enabled.
context-admin
auth-failure: Generates notifications as defined in RFC 2787 when the device in a VRRP group receives a VRRP advertisement with the authentication type or key not matching the local configuration.
new-master: Generates notifications as defined in RFC 2787 when the state of a device in a VRRP group changes from Initialize or Backup to Master.
To report critical VRRP events to an NMS, enable SNMP notifications for VRRP. For VRRP event notifications to be sent correctly, you must also configure SNMP on the device. For more information about SNMP configuration, see the network management and monitoring configuration guide for the device.
# Generate notifications as defined in RFC 2787 when the device in a VRRP group receives a VRRP advertisement with the authentication type or key not matching the local configuration.
[Sysname] snmp-agent trap enable vrrp auth-failure
vrrp check-ttl enable
Use vrrp check-ttl enable to enable TTL check for IPv4 VRRP packets.
Use undo vrrp check-ttl enable to disable TTL check for IPv4 VRRP packets.
TTL check for IPv4 VRRP packets is enabled.
Interface view
context-admin
The master in an IPv4 VRRP group periodically sends VRRP advertisements to declare its presence. The VRRP advertisements are multicast in the local subnet and cannot be forwarded by routers, so the TTL value is not changed. When the master sends VRRP advertisements, it sets the TTL value to 255. If you enable TTL check, the backups drop the VRRP advertisements with TTL other than 255, preventing attacks from other subnets.
Devices from different vendors might implement VRRP differently. When the device is interoperating with devices of other vendors, TTL check on VRRP packets might result in unexpected dropping of packets. In this scenario, use the undo vrrp check-ttl enable command to disable TTL check on VRRP packets.
# Disable TTL check for IPv4 VRRP packets.
[Sysname-GigabitEthernet1/0/1] undo vrrp check-ttl enable
vrrp dot1q
Use vrrp dot1q to specify IPv4 VRRP control VLANs.
Use undo vrrp dot1q to restore the default.
vrrp dot1q vid vlan-id
undo vrrp dot1q
No VRRP control VLANs are specified. If the ambiguous termination-enabled interface supports transmitting broadcasts/multicasts, the master sends VRRP advertisements within all VLANs whose packets are terminated by the interface.
Reth subinterface view
context-admin
vid vlan-id: Specifies an IPv4 VRRP control VLAN by its VLAN ID in the range of 1 to 4094
This command takes effect only on the following interfaces:
·     Layer 3 Ethernet subinterfaces.
·     Layer 3 aggregate subinterfaces.
·     Reth subinterfaces.
# Specify VLAN 2 as the IPv4 VRRP control VLAN.
[Sysname] interface gigabitethernet 1/0/1.2
[Sysname-GigabitEthernet1/0/1.2] vrrp dot1q vid 2
vrrp dscp
Use vrrp dscp to set a DSCP value for VRRP packets.
Use undo vrrp dscp to restore the default.
vrrp dscp dscp-value
undo vrrp dscp
The DSCP value for VRRP packets is 48.
context-admin
dscp-value: Specifies a DSCP value for VRRP packets, in the range of 0 to 63.
The DSCP value identifies the packet priority during transmission. A greater DSCP value means a higher packet priority.
# Set the DSCP value to 30 for VRRP packets.
[Sysname] vrrp dscp 30
vrrp mode
Use vrrp mode to specify the operating mode for IPv4 VRRP.
Use undo vrrp mode to restore the default.
vrrp mode load-balance [ version-8 ]
undo vrrp mode
IPv4 VRRP operates in standard mode.
context-admin
load-balance: Specifies the load balancing mode.
version-8: Specifies the version carried in VRRP packets as 8.
After you create IPv4 VRRP groups on the router, you can use this command to modify their operating mode. All IPv4 VRRP groups on the router operate in the specified mode.
The version-8 keyword takes effect only when the version of IPv4 VRRP configured on the interface is VRRPv2. The version-8 keyword is required in the following conditions:
·     A router running Comware 5 software exists in the VRRP group.
To display the software version, use the display version command.
·     All routers in the IPv4 VRRP group are operating in load balancing mode.
·     All routers in the IPv4 VRRP group are configured with the version of VRRPv2.
# Specify the load balancing mode for IPv4 VRRP.
[Sysname] vrrp mode load-balance
display vrrp
vrrp version
Use vrrp version to specify the version of IPv4 VRRP on an interface.
Use undo vrrp version to restore the default.
vrrp version version-number
undo vrrp version
VRRPv3 is used.
Interface view
context-admin
version-number: Specifies a VRRP version. The version number is 2 or 3, where 2 indicates VRRPv2 (described in RFC 3768), and 3 indicates VRRPv3 (described in RFC 5798).
The version of VRRP on all routers in an IPv4 VRRP group must be the same.
# Specify VRRPv2 to run on interface GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] vrrp version 2
vrrp vrid
Use vrrp vrid to create an IPv4 VRRP group and assign a virtual IP address to it, or to assign a virtual IP address to an existing IPv4 VRRP group.
Use undo vrrp vrid to remove all configurations of an IPv4 VRRP group, or to remove a virtual IP address from an IPv4 VRRP group.
vrrp vrid virtual-router-id virtual-ip virtual-address [ active | standby ]
undo vrrp vrid virtual-router-id [ virtual-ip [ virtual-address ] ]
No IPv4 VRRP groups exist.
Interface view
context-admin
virtual-ip virtual-address: Specifies a virtual IP address. You cannot specify the virtual IP address as any of the following IP addresses:
·     All-zero address (0.0.0.0).
·     Broadcast address (255.255.255.255).
·     Loopback address.
·     IP address of other than Class A, Class B, and Class C.
·     Invalid IP address (for example, 0.0.0.1).
If you do not specify the virtual-address argument, the undo vrrp vrid command removes all virtual IP addresses from the specified IPv4 VRRP group.
active: Associates the VRRP group with RBM by adding the device to the VRRP active group. The initial role of the device is master.
standby: Associates the VRRP group with RBM by adding the device to the VRRP standby group. The initial role of the device is backup.
You can execute this command multiple times to assign multiple virtual IP addresses to an IPv4 VRRP group. An IPv4 VRRP group can have a maximum of 16 virtual IP addresses.
An IPv4 VRRP group without virtual IP addresses configured can exist on a device provided that other settings (for example, priority and preemption mode) are available. Such a VRRP group stays in inactive state and does not function.
The virtual IP address of an IPv4 VRRP group and the downlink interface IP addresses of the VRRP group members must be in the same subnet. Otherwise, the hosts in the subnet might fail to access external networks.
For VRRP to operate correctly in load balancing mode, make sure the virtual IP address of an IPv4 VRRP group is not the IP address of any interfaces in the VRRP group.
You cannot associate a VRRP group operating in load balancing mode with RBM.
A VRRP group associated with RBM can have only one virtual IP address, and cannot contain an IP address owner.
You cannot associate a VRRP group with both RBM and Track.
To modify the settings for the command, first execute the undo form of the command, and then execute the vrrp vrid command again.
# Create IPv4 VRRP group 1 and assign virtual IP address 10.10.10.10 to the VRRP group. Then assign virtual IP address 10.10.10.11 to the VRRP group.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 virtual-ip 10.10.10.10
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 virtual-ip 10.10.10.11
display vrrp
vrrp vrid authentication-mode
Use vrrp vrid authentication-mode to configure the authentication mode and the authentication key for an IPv4 VRRP group to send and receive VRRP packets.
Use undo vrrp vrid authentication-mode to restore the default.
vrrp vrid virtual-router-id authentication-mode { md5 | simple } { cipher | plain } string
undo vrrp vrid virtual-router-id authentication-mode
Authentication is disabled when a VRRP group sends and receives VRRP packets.
Interface view
context-admin
md5: Specifies the MD5 authentication mode.
simple: Specifies the simple authentication mode.
plain: Specifies a key in plaintext form. For security purposes, the key specified in plaintext form will be stored in encrypted form.
string: Specifies the key. Its plaintext form is a case-sensitive string of 1 to 8 characters. Its encrypted form is a case-sensitive string of 1 to 41 characters.
To avoid attacks from unauthorized users, VRRP member routers add authentication keys in VRRP packets to authenticate one another. VRRP provides the following authentication modes:
·     simple—Simple text authentication.
The sender fills an authentication key into the VRRP packet, and the receiver compares the received authentication key with its local authentication key. If the two authentication keys are the same, the received VRRP packet is legitimate. Otherwise, the received packet is illegitimate.
·     md5—MD5 authentication.
The sender computes a digest for the VRRP packet by using the authentication key and MD5 algorithm, and saves the result to the authentication header. The receiver performs the same operation by using the authentication key and MD5 algorithm, and it compares the result with the content in the authentication header. If the results are the same, the received VRRP packet is legitimate. Otherwise, the received packet is illegitimate.
The MD5 authentication is more secure than the simple text authentication, but it costs more resources.
IMPORTANT
IMPORTANT:
·     You can configure different authentication modes and authentication keys for the VRRP groups on an interface. However, members of the same VRRP group must use the same authentication mode and authentication key.
·     For VRRPv3, this command does not take effect because VRRPv3 does not support authentication.
# Set the authentication mode to simple and the authentication key to Sysname for VRRP group 1 on GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 authentication-mode simple plain Sysname
display vrrp
vrrp version
vrrp vrid preempt-mode
Use vrrp vrid preempt-mode to enable the preemptive mode for the device in an IPv4 VRRP group and set the preemption delay.
Use undo vrrp vrid preempt-mode to disable the preemptive mode for the device in an IPv4 VRRP group.
Use undo vrrp vrid preempt-mode delay to restore the default preemption delay.
vrrp vrid virtual-router-id preempt-mode [ delay delay-value ]
undo vrrp vrid virtual-router-id preempt-mode [ delay ]
The device operates in preemptive mode and the preemption delay is 0 centiseconds.
Interface view
context-admin
delay delay-value: Specifies the preemption delay in the range of 0 to 180000 in centiseconds.
In non-preemptive mode, the master router acts as the master as long as it operates correctly, even if a backup is assigned a higher priority later. The non-preemptive mode helps avoid frequent switchover between the master and backups.
In preemptive mode, a backup sends VRRP advertisements when it detects that it has a higher priority than the master. Then the backup takes over as the master and the previous master becomes a backup. This mechanism ensures that the master is always the device with the highest priority.
You can configure the VRRP preemption delay for the following purposes:
·     Avoid frequent state changes among members in a VRRP group.
·     Provide the backups with enough time to collect information (such as routing information).
A backup does not immediately become the master after it receives an advertisement with a lower priority than the local priority. Instead, it waits for a period of time before taking over as the master.
# Enable the preemptive mode for the device in VRRP group 1, and set the preemption delay to 5000 centiseconds.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 preempt-mode delay 5000
display vrrp
vrrp vrid priority
Use vrrp vrid priority to set the priority of the device in an IPv4 VRRP group.
Use undo vrrp vrid priority to restore the default.
undo vrrp vrid virtual-router-id priority
The priority of a device in an IPv4 VRRP group is 100.
Interface view
context-admin
priority-value: Specifies a priority value in the range of 1 to 254. A higher value indicates a higher priority.
VRRP determines the role (master or backup) of each device in a VRRP group by priority. A device with a higher priority is more likely to become the master.
Priorities 1 to 254 are configurable. Priority 0 is reserved for special uses, and priority 255 is for the IP address owner. The IP address owner in a VRRP group always has a running priority of 255 and acts as the master as long as it operates correctly.
# Set the priority of the router to 150 in VRRP group 1 on GigabitEthernet 1/0/1.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 priority 150
display vrrp
vrrp vrid track
vrrp vrid shutdown
Use vrrp vrid shutdown to disable an IPv4 VRRP group.
Use undo vrrp vrid shutdown to enable an IPv4 VRRP group.
vrrp vrid virtual-router-id shutdown
undo vrrp vrid virtual-router-id shutdown
An IPv4 VRRP group is enabled.
Interface view
context-admin
You can use this command to temporarily disable an IPv4 VRRP group. After this command is configured, the VRRP group stays in Initialize state, and its configurations remain unchanged. You can change the configuration of the VRRP group, and your changes take effect when you enable the VRRP group again.
# Disable IPv4 VRRP group 1.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 shutdown
vrrp vrid source-interface
Use vrrp vrid source-interface to specify the source interface for an IPv4 VRRP group, instead of the interface where the VRRP group resides, to send and receive VRRP packets.
Use undo vrrp source-interface to cancel the specified source interface.
vrrp vrid virtual-router-id source-interface interface-type interface-number
undo vrrp vrid virtual-router-id source-interface
No source interface is specified for a VRRP group. The interface where the VRRP group resides sends and receives VRRP packets.
Interface view
context-admin
If VRRP group members cannot exchange VRRP packets through the interfaces where the VRRP group resides, use this command to specify interfaces for VRRP packet exchange.
# Specify GigabitEthernet 1/0/2 as the source interface for VRRP packet exchange in IPv4 VRRP group 10.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 10 source-interface gigabitethernet 1/0/2
vrrp vrid timer advertise
Use vrrp vrid timer advertise to set the interval at which the master in an IPv4 VRRP group sends VRRP advertisements.
Use undo vrrp vrid timer advertise to restore the default.
undo vrrp vrid virtual-router-id timer advertise
The master in an IPv4 VRRP group sends VRRP advertisements at an interval of 100 centiseconds.
Interface view
context-admin
adver-interval: Specifies an interval for the master in the specified IPv4 VRRP group to send VRRP advertisements. The value range for this argument is 10 to 4095 centiseconds. For VRRPv2, the value of the adver-interval argument can only be a multiple of 100. For example, if you configure values in the range of 10 to 100, 101 to 200, and 4001 to 4095, the actual values are 100, 200, and 4100, respectively. For VRRPv3, the configured value for the adver-interval argument takes effect.
The master in an IPv4 VRRP group periodically sends VRRP advertisements to declare its presence. You can use this command to configure the interval at which the master sends VRRP advertisements.
As a best practice to maintain system stability, set the VRRP advertisement interval to be greater than 100 centiseconds.
In VRRPv2, all routers in an IPv4 VRRP group must have the same interval for sending VRRP advertisements.
In VRRPv3, the routers in an IPv4 VRRP group can have different intervals for sending VRRP advertisements. The master in the VRRP group sends VRRP advertisements at the specified interval and carries the interval attribute in the advertisements. After a backup receives the advertisement, it records the interval in the advertisement. If the backup does not receive any VRRP advertisement when the timer (3 × recorded interval + Skew_Time) expires, it regards the master as failed and takes over.
Large network traffic might disable a backup from receiving VRRP advertisements from the master within the specified timer and trigger an unexpected master switchover. To solve this problem, you can use this command to set a larger interval.
# Configure the master in IPv4 VRRP group 1 to send VRRP advertisements at an interval of 500 centiseconds.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 timer advertise 500
display vrrp
vrrp vrid track
Use vrrp vrid track to associate a VRRP group or the VFs in a VRRP group with a track entry.
Use undo vrrp vrid track to remove the association between a VRRP group or the VFs in a VRRP group and a track entry.
vrrp vrid virtual-router-id track track-entry-number { forwarder-switchover member-ip ip-address | priority reduced [ priority-reduced ] | switchover | weight reduced [ weight-reduced ] }
undo vrrp vrid virtual-router-id track [ track-entry-number ] [ forwarder-switchover | priority reduced | switchover | weight reduced ]
A VRRP group and the VFs in a VRRP group are not associated with any track entries.
Interface view
context-admin
virtual-router-id: Specifies an IPv4 VRRP group number in the range of 1 to 255.
track-entry-number: Specifies a track entry by its number in the range of 1 to 1024.
forwarder-switchover member-ip ip-address: Enables the LVF on the router to take over the role of the AVF at the specified IP address immediately after the specified track entry changes to the Negative state. The ip-address argument specifies the IP address of a member router. You can use the display vrrp verbose command to view the IP addresses of the members.
priority reduced [ priority-reduced ]: Reduces the priority of the router in the VRRP group by the specified value when the state of the specified track entry changes to Negative. The value range for the priority-reduced argument is 1 to 255, and the default value is 10.
switchover: Enables the router in backup state to take over as the master immediately after the specified track entry changes to the Negative state.
weight reduced [ weight-reduced ]: Reduces the weight of all VFs on the router in the VRRP group by the specified value when the state of the specified track entry changes to Negative. The value range for the weight-reduced argument is 1 to 255, and the default value is 30.
When the associated track entry changes to the Negative state, one of the following events occurs depending on your configuration:
·     The priority of the router in the VRRP group decreases by a specified value.
·     The weight of VFs decreases by a specified value.
·     The router immediately takes over as the master if it is a backup.
·     The LVF on the router immediately takes over the role of the AVF at the specified IP address.
When the track entry changes from Negative to Positive or NotReady, one of the following events occurs:
·     The router automatically restores its priority or VF weight.
·     The failed master router becomes the master again.
·     The failed AVF becomes active again.
Before executing this command, create a VRRP group on the interface and assign a virtual IP address to the VRRP group.
You can create a track entry by using the track command before or after you associate it with a VRRP group or the VFs in a VRRP group. For more information about configuring track entries, see High Availability Configuration Guide.
If no track entry is specified, the undo vrrp vrid track command removes all associations between track entries and the VRRP group or VFs in the VRRP group.
The vrrp vrid track priority reduced command and the vrrp vrid track switchover command do not take effect on an IP address owner. If you configure the command on an IP address owner, the configuration takes effect after the router changes to be a non-IP address owner.
The following parameters take effect only when the IPv4 VRRP group is operating in load balancing mode:
·     The forwarder-switchover member-ip ip-address option.
·     The weight reduced weight-reduced option.
·     The weight reduced keyword.
The weight of a VF is 255, and its lower limit of failure is 10.
When the weight of a VF owner is higher than or equal to the lower limit of failure, its priority is always 255. The priority does not change with the weight. When the upstream link of the VF owner fails, an LVF must take over as the AVF. The switchover occurs when the weight of the VF owner drops below the lower limit of failure. This requires that the reduced weight for the VF owner be higher than 245.
# Associate VRRP group 1 on GigabitEthernet 1/0/1 with track entry 1 and decrease the router priority by 50 when the state of track entry 1 changes to Negative.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 track 1 priority reduced 50
# Associate the VFs of IPv4 VRRP group 1 on GigabitEthernet 1/0/1 with track entry 1. Enable the LVF to take over the role of the AVF at the IP address of 10.1.1.3 immediately when the state of track entry 1 changes to Negative.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 track 1 forwarder-switchover member-ip 10.1.1.3
# Associate the VFs of IPv4 VRRP group 1 on GigabitEthernet 1/0/1 with track entry 1. Decrease the weight of all VFs on the router in the VRRP group by 50 when the state of track entry 1 changes to Negative.
[Sysname-GigabitEthernet1/0/1] vrrp vrid 1 track 1 weight reduced 50
display vrrp
IPv6 VRRP commands
display vrrp ipv6
Use display vrrp ipv6 to display the states of IPv6 VRRP groups.
display vrrp ipv6 [ interface interface-type interface-number [ vrid virtual-router-id ] ] [ verbose ]
context-admin
context-operator
vrid virtual-router-id: Specifies an IPv6 VRRP group by its virtual router ID in the range of 1 to 255.
verbose: Displays detailed IPv6 VRRP group information. If you do not specify the verbose keyword, the command displays brief IPv6 VRRP group information.
If no interface or VRRP group is specified, this command displays the states of all IPv6 VRRP groups.
If only an interface is specified, this command displays the states of all IPv6 VRRP groups on the specified interface.
If both an interface and an IPv6 VRRP group are specified, this command displays the states of the specified IPv6 VRRP group on the specified interface.
# Display brief information about all IPv6 VRRP groups on the device when VRRP operates in standard mode.
<Sysname> display vrrp ipv6
IPv6 Virtual Router Information:
                                       Pri     Timer   Type        IP
 GE1/0/1            1     Master       150     100     None     FE80::1
Table 7 Command output (in standard mode)
Running Mode
VRID
Running Pri
Adver Timer
Auth Type
Authentication type. Only none is available, which means no authentication is required.
Virtual IP
# Display detailed information about all IPv6 VRRP groups on the device when VRRP operates in standard mode.
<Sysname> display vrrp ipv6 verbose
     Preempt Mode   : Yes                  Delay Time   : 10
     Auth Type      : None
     Virtual IP     : FE80::1
     Virtual MAC    : 0000-5e00-0201
     Master IP      : FE80::2
     VRID           : 2                    Adver Timer  : 100
     Become Master  : 2450ms left
     Auth Type      : None
     Virtual IP     : FE80::11
     Virtual MAC    : 0000-5e00-0202
     Master IP      : FE80::12
Table 8 Command output (in standard mode)
Running Mode
VRID
Adver Timer
Admin Status
Config Pri
Configured priority of the router, which is configured by using the vrrp ipv6 vrid priority command.
Running Pri
Preempt Mode
Preemptive mode:
·     Yes.
·     No.
Delay Time
Become Master
Auth Type
Virtual IP
Virtual MAC
Master IP
Link-local address of the interface where the master resides.
Track entry information. This field is displayed only after you configure the vrrp ipv6 vrid track command.
Track Object
Track entry state:
·     Negative.
·     Positive.
·     NotReady.
Pri Reduced
Value by which the priority decreases when the state of the associated track entry becomes Negative.
Switchover
Switchover mode. When the state of the associated track entry becomes Negative, the backup immediately becomes the master.
# Display brief information about all IPv6 VRRP groups on the device when VRRP operates in load balancing mode.
                                       Pri
 GE1/0/1            1     Master       150     FE80::1             Local
 -----              VF 1  Active       255     000f-e2ff-4011      Local
Table 9 Command output (in load balancing mode)
Running Mode
VRID
Virtual router ID (VRRP group number) or VF ID.
Running Pri
·     For a VF, this field indicates the running priority of the VF. When a track entry is associated with a VF, the priority of the VF changes if the state of the track entry changes.
Address
Active
·     For a VRRP group, this field indicates the link-local address of the interface where the master resides. If the current router is the master, this field displays local.
·     For a VF, this field indicates the link-local address of the interface where the AVF resides. If the current VF is the AVF, this field displays local.
# Display detailed information about all IPv6 VRRP groups on the device when VRRP operates in load balancing mode.
     Auth Type      : None
     Virtual IP     : FE80::10
     Member IP List : FE80::3 (Local, Master)
                      FE80::2 (Backup)
     Master IP      : FE80::3
     Config Weight  : 255
    Forwarder 01
     State          : Active
     Virtual MAC    : 000f-e2ff-4011 (Owner)
     Priority       : 255
     Active         : local
    Forwarder 02
     State          : Listening
     Virtual MAC    : 000f-e2ff-4012 (Learnt)
     Priority       : 127
     Active         : FE80::2
     Auth Type      : None
     Member IP List : FE80::3 (Local, Backup)
                      FE80::2 (Master)
     Master IP      : FE80::2
     Config Weight  : 255
    Forwarder 01
     State          : Active
     Priority       : 127
     Active         : FE80::2
    Forwarder 02
     State          : Listening
     Priority       : 255
     Active         : local
Table 10 Command output (in load balancing mode)
Running Mode
VRID
Adver Timer
Admin Status
Config Pri
Running Pri
Preempt Mode
Preemptive mode:
·     Yes.
·     No.
Delay Time
Become Master
Auth Type
Virtual IP
Member IP List
·     BackupIP address of the backup.
Track entry that is associated with the VRRP group. This field is displayed only after you configure the vrrp ipv6 vrid track command.
Track Object
Track entry to be monitored. This field is displayed only after you configure the vrrp ipv6 vrid track command.
Track entry state:
·     Negative.
·     Positive.
·     NotReady.
Pri Reduced
Value by which the priority decreases when the status of the associated track entry becomes Negative. This field is displayed only after you configure the vrrp ipv6 vrid track command.
Switchover
Switchover mode. When the status of the associated track entry becomes Negative, the backup immediately becomes the master.
VF information: Two VFs exist and one is the AVF.
Config Weight
Running Weight
Forwarder 01
VF state:
Virtual MAC
Owner ID
Priority
Active
Link-local address of the interface where the AVF resides. If the current VF is the AVF, this field displays local.
The field is displayed only after you configure the vrrp ipv6 vrid track command.
Track Object
Track entry which is associated with the VFs.
Track entry state:
·     Negative.
·     Positive.
·     NotReady.
Weight Reduced
display vrrp ipv6 statistics
Use display vrrp ipv6 statistics to display statistics for IPv6 VRRP groups.
display vrrp ipv6 statistics [ interface interface-type interface-number [ vrid virtual-router-id ] ]
context-admin
context-operator
If no interface or VRRP group is specified, this command displays statistics for all IPv6 VRRP groups.
If only an interface is specified, this command displays statistics for all IPv6 VRRP groups on the specified interface.
If both an interface and an IPv6 VRRP group are specified, this command displays statistics for the specified IPv6 VRRP group on the specified interface.
# Display statistics for all IPv6 VRRP groups when VRRP operates in standard mode.
<Sysname> display vrrp ipv6 statistics
 VRID                    : 1
 Hop Limit Errors        : 0          Advertisement Interval Errors : 0
 Adver Sent              : 425        Priority Zero Pkts Sent       : 0
 Global statistics
 CheckSum Errors         : 0
 Version Errors          : 0
 VRID Errors             : 0
# Display statistics for all IPv6 VRRP groups when VRRP operates in load balancing mode.
 VRID                    : 1
 Global statistics
 CheckSum Errors         : 0
 Version Errors          : 0
 VRID Errors             : 0
Table 11 Command output (in standard mode)
VRID
VRRP group number.
CheckSum Errors
Version Errors
Invalid Pkts Rcvd
Hop Limit Errors
Number of packets with hop limit errors.
Auth Failures
Invalid Auth Type
Auth Type Mismatch
Address List Errors
Become Master
Adver Rcvd
Adver Sent
Global statistics
Global statistics for all IPv6 VRRP groups.
CheckSum Errors
Version Errors
VRID Errors
Table 12 Command output (in load balancing mode)
VRID
VRRP group number.
CheckSum Errors
Version Errors
Invalid Pkts Rcvd
Hop Limit Errors
Auth Failures
Invalid Auth Type
Auth Type Mismatch
Address List Errors
Become Master
Become AVF
Adver Rcvd
Request Rcvd
Adver Sent
Request Sent
Reply Rcvd
Release Rcvd
Reply Sent
Release Sent
Global statistics
CheckSum Errors
Version Errors
VRID Errors
reset vrrp ipv6 statistics
Use reset vrrp ipv6 statistics to clear statistics for IPv6 VRRP groups.
reset vrrp ipv6 statistics [ interface interface-type interface-number [ vrid virtual-router-id ] ]
context-admin
If no interface or VRRP group is specified, this command clears statistics for all IPv6 VRRP groups.
If only an interface is specified, this command clears statistics for all IPv6 VRRP groups on the specified interface.
If both an interface and an IPv6 VRRP group are specified, this command clears statistics for the specified IPv6 VRRP group on the specified interface.
# Clear statistics for all IPv6 VRRP groups on all interfaces.
<Sysname> reset vrrp ipv6 statistics
vrrp ipv6 dot1q
Use vrrp ipv6 dot1q to specify IPv6 VRRP control VLANs.
Use undo vrrp ipv6 dot1q to restore the default.
vrrp ipv6 dot1q vid vlan-id
No IPv6 VRRP control VLANs are specified. If the ambiguous termination-enabled interface supports transmitting broadcasts/multicasts, the master sends IPv6 VRRP advertisements within all VLANs whose packets are terminated by the interface.
context-admin
vid vlan-id: Specifies an IPv6 VRRP control VLAN by its VLAN ID in the range of 1 to 4094.
# Specify VLAN 2 as the IPv6 VRRP control VLAN.
[Sysname-GigabitEthernet1/0/1.2] vrrp ipv6 dot1q vid 2
vrrp ipv6 dscp
Use vrrp ipv6 dscp to set a DSCP value for IPv6 VRRP packets.
Use undo vrrp ipv6 dscp to restore the default.
vrrp ipv6 dscp dscp-value
undo vrrp ipv6 dscp
The DSCP value for IPv6 VRRP packets is 56.
context-admin
dscp-value: Specifies a DSCP value for IPv6 VRRP packets, in the range of 0 to 63.
# Set the DSCP value to 30 for IPv6 VRRP packets.
[Sysname] vrrp ipv6 dscp 30
vrrp ipv6 mode
Use vrrp ipv6 mode to specify the operating mode for IPv6 VRRP.
Use undo vrrp ipv6 mode to restore the default.
vrrp ipv6 mode load-balance
undo vrrp ipv6 mode
IPv6 VRRP operates in standard mode.
context-admin
For IPv6 VRRP to operate correctly in load balancing mode, make sure the virtual IPv6 address of an IPv6 VRRP group is not the IPv6 address of any interfaces in the VRRP group.
After you create IPv6 VRRP groups on the router, you can use this command to modify their operating mode. All IPv6 VRRP groups on the router operate in the specified mode.
# Specify the load balancing mode for IPv6 VRRP.
[Sysname] vrrp ipv6 mode load-balance
display vrrp ipv6
vrrp ipv6 vrid
Use vrrp ipv6 vrid to create an IPv6 VRRP group and assign a virtual IPv6 address to it, or to assign a virtual IPv6 address to an existing IPv6 VRRP group.
Use undo vrrp ipv6 vrid to remove all configurations of an IPv6 VRRP group, or to remove a virtual IPv6 address from an IPv6 VRRP group.
vrrp ipv6 vrid virtual-router-id virtual-ip virtual-address [ link-local ]
undo vrrp ipv6 vrid virtual-router-id [ virtual-ip [ virtual-address [ link-local ] ] ]
No IPv6 VRRP groups exist.
Interface view
context-admin
virtual-ip virtual-address: Specifies a virtual IPv6 address. If you do not specify this option, the undo vrrp ipv6 vrid command removes all virtual IPv6 addresses from the specified IPv6 VRRP group.
link-local: Specifies a link-local address as the virtual IPv6 address.
You can execute this command multiple times to assign multiple virtual IPv6 addresses to an IPv6 VRRP group. An IPv6 VRRP group can have a maximum of 16 virtual IPv6 addresses.
The first virtual IPv6 address that you assign to an IPv6 VRRP group must be a link-local address, and it must be removed last.
An IPv6 VRRP group can have only one link-local address as its virtual IPv6 address.
An IPv6 VRRP group without virtual IPv6 addresses configured can exist on a device provided that other settings (for example, priority and preemption mode) are available. Such a VRRP group stays in inactive state and does not function.
The virtual IPv6 address of an IPv6 VRRP group and the downlink interface IPv6 address of the VRRP group members must be in the same subnet. Otherwise, the hosts in the subnet might fail to access external networks.
# Create IPv6 VRRP group 1 and assign virtual IPv6 address fe80::10 to the VRRP group. Then assign virtual IPv6 address 1::10 to the VRRP group.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 virtual-ip fe80::10 link-local
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 virtual-ip 1::10
display vrrp ipv6
vrrp ipv6 vrid preempt-mode
Use vrrp ipv6 vrid preempt-mode to enable the preemptive mode for the router in an IPv6 VRRP group and set the preemption delay.
Use undo vrrp ipv6 vrid preempt-mode to disable the preemptive mode for the router in an IPv6 VRRP group.
Use undo vrrp ipv6 vrid preempt-mode delay to restore the default preemption delay.
vrrp ipv6 vrid virtual-router-id preempt-mode [ delay delay-value ]
undo vrrp ipv6 vrid virtual-router-id preempt-mode [ delay ]
The router operates in preemptive mode and the preemption delay is 0 centiseconds.
Interface view
context-admin
In preemptive mode, a backup sends VRRP advertisements when it detects that it has a higher priority than the master. Then the backup takes over as the master and the previous master becomes a backup. This mechanism ensures that the master is always the router with the highest priority.
A backup does not immediately become the master after it receives an advertisement with a lower priority than the local priority. Instead, it waits for a period of time before taking over.
# Enable the preemptive mode for VRRP group 1, and set the preemption delay to 5000 centiseconds.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 10 preempt-mode delay 5000
display vrrp ipv6
Use vrrp ipv6 vrid priority to set the priority of the router in an IPv6 VRRP group.
Use undo vrrp ipv6 vrid priority to restore the default.
vrrp ipv6 vrid virtual-router-id priority priority-value
undo vrrp ipv6 vrid virtual-router-id priority
The priority of a router in an IPv6 VRRP group is 100.
Interface view
context-admin
VRRP determines the role (master or backup) of each router in a VRRP group by priority. A router with a higher priority is more likely to become the master.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 priority 150
display vrrp ipv6
vrrp ipv6 vrid shutdown
Use vrrp ipv6 vrid shutdown to disable an IPv6 VRRP group.
Use undo vrrp ipv6 vrid shutdown to enable an IPv6 VRRP group.
vrrp ipv6 vrid virtual-router-id shutdown
undo vrrp ipv6 vrid virtual-router-id shutdown
An IPv6 VRRP group is enabled.
Interface view
context-admin
You can use this command to temporarily disable an IPv6 VRRP group. After this command is configured, the VRRP group stays in Initialize state, and its configurations remain unchanged. You can change the configuration of the VRRP group, and your changes take effect when you enable the VRRP group again.
# Disable IPv6 VRRP group 1.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 shutdown
vrrp ipv6 vrid timer advertise
Use vrrp ipv6 vrid timer advertise to set the interval at which the master in an IPv6 VRRP group sends VRRP advertisements.
Use undo vrrp ipv6 vrid timer advertise to restore the default.
vrrp ipv6 vrid virtual-router-id timer advertise adver-interval
undo vrrp ipv6 vrid virtual-router-id timer advertise
The master in an IPv6 VRRP group sends VRRP advertisements at an interval of 100 centiseconds.
Interface view
context-admin
adver-interval: Specifies an interval for the master in the specified IPv6 VRRP group to send VRRP advertisements, in the range of 100 to 4095 centiseconds.
The master in an IPv6 VRRP group periodically sends VRRP advertisements to declare its presence. You can use this command to set the interval at which the master sends VRRP advertisements.
The routers in an IPv6 VRRP group can have different intervals for sending VRRP advertisements. The master in the VRRP group sends VRRP advertisements at the specified interval and carries the interval attribute in the advertisements. After a backup receives the advertisement, it records the interval in the advertisement. If the backup does not receive any VRRP advertisement when the timer (3 × VRRP advertisement sending interval + Skew_Time) expires, it regards the master as failed and takes over.
Large network traffic might disable a backup from receiving VRRP advertisements from the master within the specified timer and trigger an unexpected master switchover. To solve this problem, you can use this command to configure a larger interval.
# Configure the master in IPv6 VRRP group 1 to send VRRP advertisements at an interval of 500 centiseconds.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 timer advertise 500
display vrrp ipv6
Use vrrp ipv6 vrid track to associate an IPv6 VRRP group or the VFs in an IPv6 VRRP group with a track entry.
Use undo vrrp ipv6 vrid track to remove the association between an IPv6 VRRP group or the VFs in an IPv6 VRRP group and a track entry.
vrrp ipv6 vrid virtual-router-id track track-entry-number { forwarder-switchover member-ip ipv6-address | priority reduced [ priority-reduced ] | switchover | weight reduced [ weight-reduced ] }
undo vrrp ipv6 vrid virtual-router-id track [ track-entry-number ] [ forwarder-switchover | priority reduced | switchover | weight reduced ] ]
An IPv6 VRRP group and the VFs in an IPv6 VRRP group are not associated with any track entries.
Interface view
context-admin
virtual-router-id: Specifies an IPv6 VRRP group number in the range of 1 to 255.
forwarder-switchover member-ip ipv6-address: Enables the LVF on the router to take over the role of the AVF at the specified IPv6 address immediately after the specified track entry changes to the Negative state. The ipv6-address argument specifies the IPv6 address of a member router. You can use the display vrrp ipv6 verbose command to view the IPv6 addresses of the members.
·     The LVF on the router immediately takes over the role of the AVF at the specified IPv6 address.
Before executing this command, create an IPv6 VRRP group on the interface and assign a virtual IPv6 address to the IPv6 VRRP group.
You can create a track entry by using the track command before or after you associate it with an IPv6 VRRP group or the VFs in an IPv6 VRRP group. For more information about configuring track entries, see High Availability Configuration Guide.
If no track entry is specified, the undo vrrp ipv6 vrid track command removes all associations between track entries and the IPv6 VRRP group or VFs in the IPv6 VRRP group.
The vrrp ipv6 vrid track priority reduced command and the vrrp ipv6 vrid track switchover command do not take effect on an IP address owner. If you configure the command on an IP address owner, the configuration takes effect after the router changes to be a non-IP address owner.
The following parameters take effect only when the IPv6 VRRP group is operating in load balancing mode:
When the weight of a VF owner is higher than or equal to the lower limit of failure, its priority is always 255. The priority does not change with the weight. When the upstream link of the VF owner fails, an LVF must take over as the AVF. The switchover happens when the weight of the VF owner drops below the lower limit of failure. This requires that the reduced weight for the VF owner be higher than 245.
# Associate IPv6 VRRP group 1 on GigabitEthernet 1/0/1 with track entry 1 and decrease the router priority by 50 when the state of track entry 1 changes to Negative.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 track 1 priority reduced 50
# Associate the VFs of IPv6 VRRP group 1 on GigabitEthernet 1/0/1 with track entry 1. Enable the LVF to take over the role of the AVF at the IPv6 address of 1::3 immediately when the state of track entry 1 changes to Negative.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 track 1 forwarder-switchover member-ip 1::3
# Associate the VFs of IPv6 VRRP group 1 on GigabitEthernet 1/0/1 with track entry 1. Decrease the weight of all VFs on the router in the VRRP group by 50 when the state of track entry 1 changes to Negative.
[Sysname-GigabitEthernet1/0/1] vrrp ipv6 vrid 1 track 1 weight reduced 50
display vrrp ipv6