11-High Availability Command Reference
HomeSupportSwitchesS7500E SeriesReference GuidesCommand ReferencesH3C S7500E Switch Series Command References-Release758X-6W10011-High Availability Command Reference
04-RRPP commands
04-RRPP commands 121.58 KB
RRPP commands
control-vlan
Use control-vlan to configure the primary control VLAN for an RRPP domain.
Use undo control-vlan to restore the default.
control-vlan vlan-id
undo control-vlan
No control VLANs exist in an RRPP domain.
RRPP domain view
vlan-id: Specifies the primary control VLAN by its ID in the range of 2 to 4093.
When you configure control VLANs for an RRPP domain, you only need to configure the primary control VLAN. The system automatically configures the secondary control VLAN. It uses the primary control VLAN ID plus 1 as the secondary control VLAN ID. For the control VLAN configuration to succeed, make sure the IDs of the two control VLANs are consecutive and have not been assigned yet.
Do not configure the default VLAN of a port accessing an RRPP ring as the control VLAN.
To ensure correct forwarding of RRPPDUs, do not enable QinQ or VLAN mapping on the control VLANs.
After you configure RRPP rings for an RRPP domain, you cannot delete or modify the primary control VLAN of the domain. To do so, use the undo control-vlan command.
# Configure VLAN 100 as the primary control VLAN of RRPP domain 1 (assume that VLAN 100 and VLAN 101 have not been created yet).
[Sysname] rrpp domain 1
[Sysname-rrpp-domain1] control-vlan 100
display rrpp brief
Use display rrpp brief to display brief RRPP information.
display rrpp brief
# Display brief RRPP information.
<Sysname> display rrpp brief
 Flags for node mode: M –- Master, T -- Transit, E -- Edge, A -- Assistant-edge
 RRPP protocol status: Enabled
 Domain ID     : 1
 Control VLAN  : Primary 5, Secondary 6
 Protected VLAN: Reference instance 0 to 2, 4
 Hello timer   : 1 sec, Fail timer: 3 sec
 Linkup-Delay timer: 1 sec
  Ring  Ring   Node  Primary/Common            Secondary/Edge            Enable
  ID    level  mode  port                      port                      status
  1     1      M     XGE1/0/1                  XGE1/0/2                  Yes
 Domain ID     : 2
 Control VLAN  : Primary 10, Secondary 11
  1     0      T     XGE1/0/3                  XGE1/0/4                  Yes
  2     1      E     XGE1/0/3                  XGE1/0/5                  Yes
                     XGE1/0/4
Flags for node mode
RRPP node mode:
·     M—Master node.
·     T—Transit node.
·     E—Edge node.
·     A—Assistant edge node.
RRPP status:
·     Enabled—Globally enabled.
·     Disabled—Globally disabled.
Domain ID
RRPP domain ID.
Control VLAN
Primary and secondary control VLANs of the RRPP domain.
Protected VLAN
MSTIs corresponding to the VLANs protected by the RRPP domain. To view the VLAN-to-instance mappings, use the display stp region-configuration command (see Layer 2—LAN Switching Command Reference).
Hello timer
Hello timer value in seconds.
Fail timer
Fail timer value in seconds.
Linkup-Delay timer
Link-up delay timer value in seconds.
Ring ID
RRPP ring ID.
Ring level
RRPP ring level:
·     0—Primary ring.
·     1—Subring.
Primary/Common port
This field displays primary ports when the node mode is master node or transit node.
This field displays common ports when the node mode is edge node or assistant edge node.
A hyphen (-) appears when one of the following cases occurs:
·     The port is not configured on the ring.
·     The card to which the port belongs has not started up.
·     The port is a member of a link aggregation group.
Secondary/Edge port
This field displays secondary ports when the node mode is master node or transit node.
This field displays edge ports when the node mode is edge node or assistant edge node.
Enable status
RRPP ring status:
·     Yes—Enabled.
·     No—Disabled.
display rrpp ring-group
Use display rrpp ring-group to display the RRPP ring group configuration.
display rrpp ring-group [ ring-group-id ]
ring-group-id: Specifies an RRPP ring group by its ID in the range of 1 to 64 If you do not specify this argument, the command displays the configuration of all ring groups.
For an edge node RRPP ring group, this command also displays the subring sending Edge-Hello packets.
# Display the configuration of all RRPP ring groups.
<Sysname> display rrpp ring-group
 Ring group 1:
  Domain 1 ring 1 to 3, 5
  Domain 2 ring 1 to 3, 5
  Domain 1 ring 1 is the sending ring
 Ring group 2:
  Domain 1 ring 4, 6 to 7
  Domain 2 ring 4, 6 to 7
Ring group 1
RRPP ring group 1.
Subrings in the ring group, including rings 1, 2, 3, and 5 in RRPP domain 1.
The sending ring of the ring group is ring 1 in RRPP domain 1.
display rrpp statistics
Use display rrpp statistics to display RRPPDU statistics.
display rrpp statistics domain domain-id [ ring ring-id ]
domain domain-id: Specifies an RRPP domain by its ID in the range of 1 to 128.
ring ring-id: Specifies an RRPP ring by its ID in the range of 1 to 128. If you do not specify this option, the command displays the RRPPDU statistics for all rings in the specified RRPP domain.
If a port belongs to more than one ring, this command collects and displays RRPPDU statistics of the port by ring.
When a ring transits from inactive status to active status, packet counting for the ring restarts.
# Display RRPPDU statistics for all rings in RRPP domain 2.
<Sysname> display rrpp statistics domain 2
 Ring ID       : 1
 Ring level    : 0
 Node mode     : Master
 Active status : Yes
 Primary port  : XGE1/0/3
  Direct Hello     Link     Common     Complete   Edge      Major     Total
                   down     flush FDB  flush FDB  hello     fault
  Out    16924     0        0          1          0         0         16925
  In     0         0        0          0          0         0         0
 Secondary port: XGE1/0/4
  Out    0         0        0          0          0         0         0
  In     16878     0        0          1          0         0         16879
 Ring ID       : 2
 Ring level    : 1
 Node mode     : Edge
 Active status : No
 Common port   : XGE1/0/3
  Out    0         0        0          0          0         0         0
  In     0         0        0          0          0         0         0
 Common port   : XGE1/0/4
  Out    0         0        0          0          0         0         0
  In     0         0        0          0          0         0         0
 Edge port     : XGE1/0/5
  Out    0         0        0          0          0         0         0
  In     0         0        0          0          0         0         0
Ring ID
RRPP ring ID.
Ring level
RRPP ring level:
·     0—Primary ring.
·     1—Subring.
Node mode
Node mode:
·     Master node.
·     Transit node.
·     Edge node.
·     Assistant edge node.
Active status
RRPP ring status:
·     Yes—Active.
·     No—Inactive.
Primary port
The primary port field means the node mode is master node or transit node.
Secondary port
The secondary port field means the node mode is master node or transit node.
Common port
The common port field means the node mode is edge node or assistant edge node.
Edge port
The edge port field means the node mode is edge node or assistant edge node.
Packet direct
Packet transmission direction on the port:
·     Out—Packet sending direction.
·     In—Packet receiving direction.
Hello
Statistics of Hello packets received/sent on the port.
Link down
Statistics of Link-Down packets received/sent on the port.
Common flush FDB
Statistics of Common-Flush-FDB packets received/sent on the port.
Complete flush FDB
Statistics of Complete-Flush-FDB packets received/sent on the port.
Edge hello
Statistics of Edge-Hello packets received/sent on the port.
Major fault
Statistics of Major-Fault packets received/sent on the port.
Total
Total number of packets received/sent on the port. Only Hello, Link-Down, Common-Flush-FDB, Complete-Flush-FDB, Edge-Hello, and Major-Fault packets of RRPP are counted.
reset rrpp statistics
display rrpp verbose
Use display rrpp verbose to display detailed RRPP information.
display rrpp verbose domain domain-id [ ring ring-id ]
ring ring-id: Specifies an RRPP ring by its ID in the range of 1 to 128. If you do not specify this option, the command displays detailed information for all rings in the specified RRPP domain.
# Display detailed information for all rings in RRPP domain 2.
<Sysname> display rrpp verbose domain 2
 Domain ID     : 2
 Protected VLAN: Reference instance 3, 5 to 7
 Ring ID       : 1
 Ring level    : 0
 Node mode     : Master
 Ring state    : Completed
 Enable status : Yes, Active status: Yes
 Primary port  : XGE1/0/4                    Port status: UP
 Secondary port: XGE1/0/5                    Port status: BLOCKED
 Ring ID       : 2
 Ring level    : 1
 Node mode     : Edge
 Ring state    : Unknown
 Enable status : No, Active status: No
 Common port   : XGE1/0/4                    Port status: -
                 XGE1/0/5                    Port status: -
 Edge port     : XGE1/0/3                    Port status: -
Domain ID
RRPP domain ID.
Control VLAN
Control VLANs of the RRPP domain:
·     Primary—Primary control VLAN.
·     Secondary—Secondary control VLAN.
Protected VLAN
Hello timer
Fail timer
Linkup-Delay timer
Ring ID
RRPP ring ID.
Ring level
RRPP ring level:
·     0—Primary ring.
·     1—Subring.
Node mode
Node mode:
·     Master node.
·     Transit node.
·     Edge node.
Ring state
RRPP ring state:
·     Possible states on the master node:
¡     Completed—The ring is healthy.
¡     Failed—The ring is not closed.
¡     Unknown—The RRPP domain is disabled.
·     Possible states on a transit node or edge node:
¡     LinkUp—All ports on the node are up.
¡     LinkDown—At least one port on the node is down.
¡     PreForward—A port on the node is blocked.
·     Possible states on an assistant edge node:
¡     LinkUpNotify—The node does not receive Edge-Hello packets in LinkUp state.
¡     LinkDnNotify—The node does not receive Edge-Hello packets in LinkDown state.
¡     PreForwardNotify—The port on the directly connected edge node comes up, or the assistant edge node does not receive Edge-Hello packets in PreForward state.
If the ring is not enabled on the device operating as the master node or the device is not the master node of the ring, a hyphen (-) is displayed.
Enable status
RRPP ring status:
·     Yes—Enabled.
·     No—Disabled.
Active status
RRPP ring status:
·     Yes—Active.
·     No—Inactive.
An RRPP ring can be active only when RRPP and the RRPP ring are both enabled. This field also helps you identify whether RRPP is enabled.
Primary port
Secondary port
Common port
Edge port
Port status
Port status: Down, up, or blocked.
·     The ring is inactive.
domain ring
Use domain ring to configure subrings for an RRPP ring group.
Use undo domain ring to remove subrings from the RRPP ring group.
domain domain-id ring ring-id-list
undo domain domain-id [ ring ring-id-list ]
No subrings exist in an RRPP ring group.
RRPP ring group view
ring ring-id-list: Specifies a space-separated list of up to 10 RRPP subring ID items. Each item specifies an RRPP subring ID or a range of RRPP subring IDs. The value range for RRPP subring IDs is 1 to 128. If you do not specify this option, the command removes all subrings from the ring group in the specified domain.
Follow these guidelines when you configure an RRPP ring group on the edge node and the assistant edge node:
·     When you assign an active ring to a ring group, assign it on the assistant edge node first and then on the edge node.
·     To remove an active ring from a ring group, remove it on the edge node first and then on the assistant edge node.
·     To remove a ring group, remove it on the edge node first and then on the assistant edge node.
·     When you activate rings in a ring group, activate them on the edge node first and then on the assistant edge node.
·     When you deactivate rings in a ring group, deactivate them on the assistant edge node first and then on the edge node.
If you do not follow these guidelines, the assistant edge node might fail to receive Edge-Hello packets and consider the primary ring failed even if it did not.
# Create RRPP ring group 1, and add subrings 1, 2, 3, and 5 to domain 1 and domain 2.
[Sysname] rrpp ring-group 1
[Sysname-ring-group1] domain 1 ring 1 to 3 5
[Sysname-ring-group1] domain 2 ring 1 to 3 5
rrpp ring-group
linkup-delay-timer
Use linkup-delay-timer to set the link-up delay timer.
Use undo linkup-delay-timer to restore the default.
linkup-delay-timer delay-time [ distribute ]
The link-up delay timer is 0 seconds, and the distribute keyword is not specified.
RRPP domain view
delay-time: Specifies the link-up delay timer in the range of 0 to 30 seconds.
distribute: Enables all nodes in the RRPP domain to learn the link-up delay timer value.
The link-up delay timer prevents frequent switchover of RRPP traffic forwarding paths caused by unstable RRPP port states.
You can configure this command on any node in an RRPP domain, but this command can take effect only on the master node.
If you specify the distribute keyword in an RRPP network implementing load balancing, you must configure the link-up delay timer for each RRPP domain for the timer to take effect. If you set different timer values for different RRPP domains, the smallest timer value takes effect.
If the distribute keyword is not specified, the link-up delay timer value cannot be greater than the Fail timer value minus twice the Hello timer value.
# Set the link-up delay timer to 10 seconds for RRPP domain 1.
[Sysname-rrpp-domain1] linkup-delay-timer 10
timer
protected-vlan
Use protected-vlan to configure the protected VLANs for an RRPP domain.
Use undo protected-vlan to remove the protected VLANs from an RRPP domain.
undo protected-vlan [ reference-instance instance-id-list ]
No protected VLANs exist in an RRPP domain.
RRPP domain view
reference-instance instance-id-list: Specifies the Multiple Spanning Tree Instances (MSTIs) you want to reference in the form of instance-id-list = { instance-id [ to instance-id ] }&<1-10>. The instance-id argument is an MSTI ID in the range of 0 to 4094. You can specify up to 10 MSTI IDs or ID ranges. You can use the display stp region-configuration command to display the VLAN-to-instance mappings. If you do not specify this option, the command removes all MSTIs referenced by the RRPP domain.
You can delete or modify the protected VLANs configured for an RRPP domain before and after you configure rings for the domain. However, after you configure rings for the RRPP domain, you cannot delete configurations of all the protected VLANs configured for the domain.
When the VLAN-to-instance mappings change, the protected VLANs of an RRPP domain also change.
# Map VLANs 1 through 30 to MSTI 1, and activate the MST region configuration. Configure VLAN 100 as the control VLAN of RRPP domain 1. Configure VLANs mapped to MSTI 1 as the primary control VLANs of RRPP domain 1.
[Sysname-mst-region] instance 1 vlan 1 to 30
[Sysname-mst-region] quit
[Sysname-rrpp-domain1] protected-vlan reference-instance 1
display stp region-configuration (Layer 2—LAN Switching Command Reference)
rrpp domain
Use reset rrpp statistics to clear RRPPDU statistics.
reset rrpp statistics domain domain-id [ ring ring-id ]
ring ring-id: Specifies an RRPP ring by its ID in the range of 1 to 128. If you do not specify this option, the command clears RRPPDU statistics of all RRPP rings in the specified RRPP domain.
# Clear the RRPPDU statistics of ring 10 in RRPP domain 1.
<Sysname> reset rrpp statistics domain 1 ring 10
ring
Use ring to configure the node mode of the device, the role of the specified RRPP port, and the level of the RRPP ring.
Use undo ring to delete the RRPP ring.
ring ring-id node-mode { { master | transit } [ primary-port interface-type interface-number ] [ secondary-port interface-type interface-number ] level level-value | { assistant-edge | edge } [ edge-port interface-type interface-number ] }
undo ring ring-id
The device is not a node of the RRPP ring.
RRPP domain view
master: Specifies the device as the master node of the RRPP ring.
transit: Specifies the device as the transit node of the RRPP ring.
primary-port: Specifies the port as a primary port.
interface-type interface-number: Specifies a port by its type and number.
secondary-port: Specifies the port as a secondary port.
level level-value: Specifies an RRPP ring level, 0 for the primary ring and 1 for the subring.
assistant-edge: Specifies the device as the assistant edge node of the RRPP ring.
edge: Specifies the device as the edge node of the RRPP ring.
edge-port: Specifies the edge port for the node.
The ID of an RRPP ring in a domain must be unique.
When an RRPP ring is activated, you cannot configure its RRPP ports.
When you configure the edge node and the assistant edge node, first configure the primary ring, and then the subrings.
The node mode, RRPP port role, and ring level settings of an RRPP ring cannot be modified after they are configured. To modify the settings, first remove the current settings.
Remove all subring configurations before you delete the primary ring configuration of the edge node or the assistant edge node. However, an active RRPP ring cannot be deleted.
When RRPP is enabled on a device, you must disable the RRPP ring before you can delete it. When RRPP is disabled on the device, you can directly delete the RRPP ring, as well as the setting of the ring enable command.
Do not assign a port to both an aggregation group and an RRPP ring. If you do so, the port does not take effect on the RRPP ring.
# Specify the device as the master node of primary ring 10 in RRPP domain 1. Specify Ten-GigabitEthernet 1/0/1 as the primary port and Ten-GigabitEthernet 1/0/2 as the secondary port.
[Sysname-rrpp-domain1] protected-vlan reference-instance 0 1 2
[Sysname-rrpp-domain1] ring 10 node-mode master primary-port ten-gigabitethernet 1/0/1 secondary-port ten-gigabitethernet 1/0/2 level 0
# Specify the device as the transit node of primary ring 10 in RRPP domain 1. Specify Ten-GigabitEthernet 1/0/1 as the primary port and Ten-GigabitEthernet 1/0/2 as the secondary port. Specify the device as the edge node of subring 20 in RRPP domain 1, and specify Ten-GigabitEthernet 1/0/3 as the edge port.
[Sysname-rrpp-domain1] ring 10 node-mode transit primary-port ten-gigabitethernet 1/0/1 secondary-port ten-gigabitethernet 1/0/2 level 0
[Sysname-rrpp-domain1] ring 20 node-mode edge edge-port ten-gigabitethernet 1/0/3
ring enable
ring enable
Use ring enable to enable an RRPP ring.
Use undo ring enable to disable the RRPP ring.
ring ring-id enable
undo ring ring-id enable
An RRPP ring is disabled.
RRPP domain view
To activate an RRPP ring, you must enable RRPP and the RRPP ring.
Before you enable subrings on a device, you must enable the primary ring. Before you disable the primary ring on the device, you must disable all subrings. Otherwise, the system displays error prompts.
# Enable RRPP ring 10 in RRPP domain 1.
[Sysname-rrpp-domain1] ring 10 enable
rrpp enable
rrpp domain
Use rrpp domain to create an RRPP domain and enter its view, or enter the view of an existing RRPP domain.
Use undo rrpp domain to remove an RRPP domain.
rrpp domain domain-id
undo rrpp domain domain-id
No RRPP domains exist.
When you delete an RRPP domain, configurations of the control VLANs and protected VLANs are deleted at the same time.
To delete an RRPP domain successfully, make sure it has no RRPP rings.
# Create RRPP domain 1, and enter RRPP domain 1 view.
control-vlan
protected-vlan
rrpp enable
Use rrpp enable to enable RRPP.
Use undo rrpp enable to disable RRPP.
rrpp enable
undo rrpp enable
RRPP is disabled.
To activate an RRPP domain, enable RRPP and the RRPP rings for the RRPP domain.
# Enable RRPP.
[Sysname] rrpp enable
ring enable
rrpp ring-group
Use rrpp ring-group to create an RRPP ring group and enter its view, or enter the view of an existing RRPP ring group.
Use undo rrpp ring-group to remove an RRPP ring group.
rrpp ring-group ring-group-id
undo rrpp ring-group ring-group-id
No RRPP ring groups exist.
ring-group-id: Specifies an RRPP ring group ID in the range of 1 to 64.
When you remove a ring group, remove it on the edge node first and then on the assistant edge node. Otherwise, the assistant edge node might fail to receive Edge-Hello packets and consider the primary ring failed even if it is not.
After a ring group is removed, all subrings in the ring group do not belong to any ring group.
# Create RRPP ring group 1 and enter its view.
domain ring
snmp-agent trap enable rrpp
Use snmp-agent trap enable rrpp to enable SNMP notifications for RRPP.
Use undo snmp-agent trap enable rrpp to disable SNMP notifications for RRPP.
snmp-agent trap enable rrpp [ major-fault | multi-master | ring-fail | ring-recover ] *
undo snmp-agent trap enable rrpp [ major-fault | multi-master | ring-fail | ring-recover ] *
SNMP notifications for RRPP are disabled.
major-fault: Generates notifications when an SRPT between the assistant edge node and edge node is disconnected.
multi-master: Generates notifications when multiple master nodes are configured for the RRPP ring.
ring-fail: Generates notifications when the state of the RRPP ring changes from Health to Disconnect.
ring-recover: Generates notifications when the state of the RRPP ring changes from Disconnect to Health.
To report critical RRPP events to an NMS, enable SNMP notifications for RRPP. For RRPP event notifications to be sent correctly, you must also configure SNMP on the device. For more information about SNMP configuration, see the network management and monitoring configuration guide for the device.
If you do not specify any keyword, this command enables or disables all SNMP notifications for RRPP.
# Generate notifications when the state of the RRPP ring changes from Disconnect to Health.
[Sysname] snmp-agent trap enable rrpp ring-recover
timer
Use timer to set the Hello timer and the Fail timer.
Use undo timer to restore the default.
timer hello-timer hello-value fail-timer fail-value
undo timer
The Hello timer is 1 second and the Fail timer is 3 seconds.
RRPP domain view
hello-timer hello-value: Specifies the Hello timer in the range of 1 to 10 seconds.
fail-timer fail-value: Specifies the Fail timer in the range of 3 to 30 seconds.
The Fail timer must be greater than or equal to three times the Hello timer.
# Set the Hello timer to 2 seconds and the Fail timer to 7 seconds for RRPP domain 1.
[Sysname-rrpp-domain1] timer hello-timer 2 fail-timer 7