- 11-Network Management and Monitoring Command Reference
- 02-NQA commands
- 03-NTP commands
- 04-PoE commands
- 05-SNMP commands
- 06-RMON commands
- 07-Event MIB commands
- 08-NETCONF commands
- 09-CWMP commands
- 10-EAA commands
- 11-Process monitoring and maintenance commands
- 12-Mirroring commands
- 13-sFlow commands
- 14-Information center commands
- 15-Packet capture commands
| 05-SNMP commands | 239.37 KB |
display snmp-agent local-engineid
snmp-agent { inform | trap } source
snmp-agent trap if-mib link extended
snmp-agent usm-user { v1 | v2c }
snmp-agent usm-user v3 user-role
SNMP commands
The SNMP agent sends notifications (traps and informs) to inform the NMS of significant events, such as link state changes and user logins or logouts. Unless otherwise stated, the trap keyword in the command line includes both traps and informs.
display snmp-agent community
Use display snmp-agent community to display information about SNMPv1 or SNMPv2c communities.
read: Specifies SNMP read-only communities.
write: Specifies SNMP read and write communities.
This command is not available in FIPS mode.
If you do not specify the read or write keyword, this command displays information about all SNMPv1 and SNMPv2c communities.
This command displays SNMPv1 and SNMPv2c communities created in the following ways:
· Created by using the snmp-agent community command.
· Automatically created by the system for SNMPv1 and SNMPv2c users that have been assigned to an existing SNMP group.
# Display information about all SNMPv1 and SNMPv2c communities.
<Sysname> display snmp-agent community
Community name: aa
Group name: aa
ACL:2001
Storage-type: nonVolatile
Context name: con1
Community name: bb
Role name: bb
Community name: userv1
Group name: testv1
Storage-type: nonvolatile
Community name: cc
Group name: cc
ACL name: testacl
Community name |
Community name created by using the snmp-agent community command or username created by using the snmp-agent usm-user { v1 | v2c } command. |
Group name |
SNMP group name. · If the community is created by using the snmp-agent community command in VACM mode, the group name is the same as the community name. · If the community is created by using the snmp-agent usm-user { v1 | v2c } command, the name of the group that has the user is displayed. |
Role name |
User role name for the community. If the community is created by using the snmp-agent community command in RBAC mode, a user role can be bound to the community name. |
ACL |
Number of the ACL. This field appears only when an ACL is specified for the SNMPv1 or SNMPv2c community. It is exclusive with the ACL name field. |
ACL name |
Name of the ACL. This field appears only when an ACL is specified for the SNMPv1 or SNMPv2c community. It is exclusive with the ACL field. |
Storage-type |
Storage type: · volatile—Settings are lost when the system reboots. · nonVolatile—Settings remain after the system reboots. · permanent—Settings remain after the system reboots and can be modified but not deleted. · readOnly—Settings remain after the system reboots and cannot be modified or deleted. · other—Any other storage type. |
Context name |
SNMP context: · If a mapping between the SNMP community and an SNMP context is configured, the SNMP context is displayed. · If no mapping between the SNMP community and an SNMP context exists, this field is empty. |
display snmp-agent context
Use display snmp-agent context to display SNMP contexts.
display snmp-agent context [ context-name ]
context-name: Specifies an SNMP context by its name, a case-sensitive string of 1 to 32 characters. If you do not specify this argument, the command displays all SNMP contexts.
# Display all SNMP contexts.
<Sysname> display snmp-agent context
testcontext
snmp-agent context
display snmp-agent group
Use display snmp-agent group to display information about SNMP groups.
display snmp-agent group [ group-name ]
group-name: Specifies an SNMPv1, SNMPv2c, or SNMPv3 group name in non-FIPS mode, and an SNMPv3 group name in FIPS mode. It is a case-sensitive string of 1 to 32 characters. If you do not specify a group, this command displays information about all SNMP groups.
# Display information about all SNMP groups.
<Sysname> display snmp-agent group
Group name: groupv3
Security model: v3 noAuthnoPriv
Readview: ViewDefault
Writeview: <no specified>
Notifyview: <no specified>
ACL name: testacl
Group name |
SNMP group name. |
Security model |
Security model of the SNMP group: · authPriv—Authentication with privacy. · authNoPriv—Authentication without privacy. · noAuthNoPriv—No authentication, no privacy. Security model of an SNMPv1 or SNMPv2c group can only be noAuthNoPriv. |
Readview |
Read-only MIB view accessible to the SNMP group. |
Writeview |
Write MIB view accessible to the SNMP group. |
Notifyview |
Notify MIB view for the SNMP group. The SNMP users in the group can send notifications only for the nodes in the notify MIB view. |
Storage-type |
Storage type, including volatile, nonvolatile, permanent, readOnly, and other. For more information, see Table 1. |
ACL |
Number of the ACL. This field appears only when an ACL is specified for the SNMP group. It is exclusive with the ACL name field. |
ACL name |
Name of the ACL. This field appears only when an ACL is specified for the SNMP group. It is exclusive with the ACL field. |
snmp-agent group
Use display snmp-agent local-engineid to display the local SNMP engine ID.
Every SNMP entity has one SNMP engine to provide services for sending and receiving messages, authenticating and encrypting messages, and controlling access to managed objects.
An SNMP engine ID uniquely identifies an SNMP entity in an SNMP domain.
# Display the local SNMP engine ID.
<Sysname> display snmp-agent local-engineid
SNMP local engine ID: 800063A2800084E52BED7900000001
display snmp-agent mib-node
Use display snmp-agent mib-node to display SNMP MIB node information.
display snmp-agent mib-node [ details | index-node | trap-node | verbose ]
details: Specifies detailed MIB node information, including node name, last octet of an OID string, and name of the next leaf node.
index-node: Specifies SNMP MIB tables, and node names and OIDs of MIB index nodes.
trap-node: Specifies node names and OIDs of MIB notification nodes, and node names and OIDs of notification objects.
verbose: Specifies detailed information about SNMP MIB nodes, including node names, OIDs, node types, permissions to MIB nodes, data types, MORs, and parent, child, and sibling nodes.
If you do not specify any keywords, this command displays information about all SNMP MIB nodes, including node name, OID, and permissions to MIB nodes.
The SNMP software package includes different MIB files. Support for MIBs varies by SNMP software versions.
# Display SNMP MIB node information.
<Sysname> display snmp-agent mib-node
iso<1>(NA)
|-std<1.0>(NA)
|-iso8802<1.0.8802>(NA)
|-ieee802dot1<1.0.8802.1>(NA)
|-ieee802dot1mibs<1.0.8802.1.1>(NA)
-std |
MIB node name. |
<1.0> |
OID of a MIB node. |
(NA) |
Permissions to MIB nodes: · NA—Not accessible. · NF—Notifications. · RO—Read-only access. · RW—Read and write access. · RC—Read-write-create access. · WO—Write-only access. |
Leaf node or MIB table node. |
# Display detailed MIB node information.
<Sysname> display snmp-agent mib-node details
iso(1)(dot1xPaeSystemAuthControl)
|-std(0)(dot1xPaeSystemAuthControl)
|-iso8802(8802)(dot1xPaeSystemAuthControl)
|-ieee802dot1(1)(dot1xPaeSystemAuthControl)
|-ieee802dot1mibs(1)(dot1xPaeSystemAuthControl)
-std |
MIB node name. |
(0) |
Last bit of a MIB OID string. |
(lldpMessageTxInterval) |
Name of a leaf node. |
# Display MIB table names, and node names and OIDs of MIB index nodes.
<Sysname> display snmp-agent mib-node index-node
Table |dot1xPaePortTable
Index ||dot1xPaePortNumber
OID ||| 1.0.8802.1.1.1.1.1.2.1.1
Table 5 Command output
Table |
MIB table name. |
Index |
Name of a MIB index node. |
OID |
OID of a MIB index node. |
# Display names and OIDs of MIB notification nodes, and names and OIDs of notification objects.
<Sysname> display snmp-agent mib-node trap-node
Name |lldpRemTablesChange
OID ||1.0.8802.1.1.2.0.0.1
Trap Object
Name |||lldpStatsRemTablesInserts
OID ||||1.0.8802.1.1.2.1.2.2
Name |||lldpStatsRemTablesDeletes
OID ||||1.0.8802.1.1.2.1.2.3
Name |||lldpStatsRemTablesDrops
OID ||||1.0.8802.1.1.2.1.2.4
Name |||lldpStatsRemTablesAgeouts
OID ||||1.0.8802.1.1.2.1.2.5
Table 6 Command output
Name |
Name of a MIB notification node. |
OID |
OID of a MIB notification node. |
Trap Object |
Name and OID of a notification object. |
# Display detailed information about SNMP MIB nodes, including node names, OIDs, node types, permissions to MIB nodes, data types, MORs, and parent, child, and sibling nodes.
<Sysname> display snmp-agent mib-node verbose
Name |iso
OID ||1
Properties ||NodeType: Other
||AccessType: NA
||DataType: NA
||MOR: 0x00000000
Parent ||
First child ||std
Next leaf ||dot1xPaeSystemAuthControl
Next sibling ||
Table 7 Command output
Name |
MIB node name. |
OID |
NodeType |
MIB node types: · Table—Table node. · Row—Row node in a MIB table. · Column—Column node in a MIB table. · Leaf—Leaf node. · Group—Group node (parent node of a leaf node). · Trapnode—Notification node. · Other—Other node types. |
AccessType |
Permissions to MIB nodes: · NA—Not accessible. · NF—Supports notifications. · RO—Supports read-only access. · RW—Supports read and write access. · RC—Supports read-write-create access. · WO—Supports write-only access. |
DataType |
Data types of MIB nodes: · Integer—An integer. · Integer32—A 32-bit integer. · Unsigned32—A 32-bit integer with no mathematical sign. · Gauge—A non-negative integer that might increase or decrease. · Gauge32—A 32-bit non-negative integer that might increase or decrease. · Counter—A non-negative integer that might increase but not decrease. · Counter32—A 32-bit non-negative integer that might increase but not decrease. · Counter64—A 64-bit non-negative integer that might increase but not decrease. · Timeticks—A non-negative integer for time keeping. · Octstring—An octal string. · OID—Object identifier. · IPaddress—A 32-bit IP address. · Networkaddress—A network IP address. · Opaque—Any data. · Userdefined—User-defined data. · BITS—Bit enumeration. |
MOR |
MOR for a MIB node. |
Parent |
Name of a parent node. |
First child |
Name of the first leaf node. |
Next leaf |
Name of the next leaf node. |
Next sibling |
Name of the next sibling node. |
Allow |
Operation types allowed: · get/set/getnext—All operations. · get—Get operation. · set—Set operation. · getnext—GetNext operation. |
Value range |
Value range of a MIB node. |
Index |
Table index. This field appears only for a table node. |
display snmp-agent mib-view
Use display snmp-agent mib-view to display MIB views.
display snmp-agent mib-view [ exclude | include | viewname view-name ]
exclude: Displays the subtrees excluded from any MIB view.
include: Displays the subtrees included in any MIB view.
viewname view-name: Displays information about the specified MIB view. The view-name argument is a case-sensitive string of 1 to 32 characters.
If you do not specify any parameters, this command displays all MIB views.
# Display all MIB views.
<Sysname> display snmp-agent mib-view
View name: ViewDefault
MIB Subtree: iso
Subtree mask:
View Type: included
View status: active
MIB Subtree: snmpUsmMIB
Subtree mask:
View Type: excluded
View status: active
MIB Subtree: snmpVacmMIB
Subtree mask:
View Type: excluded
View status: active
MIB Subtree: snmpModules.18
Subtree mask:
View Type: excluded
View status: active
ViewDefault is the default MIB view. The output shows that except for the MIB objects in the snmpUsmMIB, snmpVacmMIB, and snmpModules.18 subtrees, all the MIB objects in the iso subtree are accessible.
Table 8 Command output
View name |
MIB view name. |
MIB Subtree |
MIB subtree covered by the MIB view. |
Subtree mask |
MIB subtree mask. |
Storage-type |
Type of the medium (see Table 1) where the subtree view is stored. |
View Type |
Access privilege for the MIB subtree in the MIB view: · Included—All objects in the MIB subtree are accessible in the MIB view. · Excluded—None of the objects in the MIB subtree is accessible in the MIB view. |
View status |
Status of the MIB view: · active—MIB view is effective. · inactive—MIB view is ineffective. The objects in the MIB view are not accessible, but they can send notifications. |
snmp-agent mib-view
display snmp-agent remote
Use display snmp-agent remote to display engine IDs of the remote SNMP entities.
display snmp-agent remote [ { ipv4-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ] ]
ipv4-address: Specifies a remote SNMP entity by its IPv4 address.
ipv6 ipv6-address: Specifies a remote SNMP entity by its IPv6 address.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the remote SNMP entity belongs. The vpn-instance-name argument represents the VPN instance name, a case-sensitive string of 1 to 31 characters. If the remote SNMP entity belongs to the public network, do not specify this option.
If you do not specify a remote SNMP entity, this command displays the engine IDs of all remote SNMP entities.
# Display engine IDs of all remote SNMP entities.
<Sysname> display snmp-agent remote
Remote engineID: 800063A28000A0FC00580400000001
IPv4 address: 1.1.1.1
VPN instance: vpn1
Table 9 Command output
Remote engineID |
Remote SNMP engine ID you have configured using the snmp-agent remote command. |
IPv4 address |
IPv4 address of the remote SNMP entity. |
IPv6 address |
IPv6 address of the remote SNMP entity. This field is displayed if the remote SNMP entity is configured with an IPv6 address. |
VPN instance |
This field is available only if a VPN instance has been specified for the remote SNMP entity in the snmp-agent remote command. |
snmp-agent remote
display snmp-agent statistics
Use display snmp-agent statistics to display SNMP message statistics.
# Display SNMP message statistics.
<Sysname> display snmp-agent statistics
1684 messages delivered to the SNMP entity.
5 messages were for an unsupported version.
0 messages used an unknown SNMP community name.
0 messages represented an illegal operation for the community supplied.
0 ASN.1 or BER errors in the process of decoding.
1679 messages passed from the SNMP entity.
0 SNMP PDUs had badValue error-status.
0 SNMP PDUs had genErr error-status.
0 SNMP PDUs had noSuchName error-status.
0 SNMP PDUs had tooBig error-status (Maximum packet size 1500).
16544 MIB objects retrieved successfully.
2 MIB objects altered successfully.
7 GetRequest-PDU accepted and processed.
7 GetNextRequest-PDU accepted and processed.
1653 GetBulkRequest-PDU accepted and processed.
1669 GetResponse-PDU accepted and processed.
2 SetRequest-PDU accepted and processed.
0 Trap PDUs accepted and processed.
0 alternate Response Class PDUs dropped silently.
0 forwarded Confirmed Class PDUs dropped silently.
Table 10 Command output
messages delivered to the SNMP entity |
Number of messages that the SNMP agent has received. |
messages were for an unsupported version |
Number of messages that are not supported by the SNMP agent version. |
messages used an unknown SNMP community name |
Number of messages that used an unknown SNMP community name. |
messages represented an illegal operation for the community supplied |
Number of messages carrying an operation that the community has no right to perform. |
ASN.1 or BER errors in the process of decoding |
Number of messages that had ASN.1 or BER errors during decoding. |
messages passed from the SNMP entity |
Number of messages sent by the SNMP agent. |
SNMP PDUs had badValue error-status |
Number of PDUs with a BadValue error. |
SNMP PDUs had genErr error-status |
Number of PDUs with a genErr error. |
SNMP PDUs had noSuchName error-status |
Number of PDUs with a NoSuchName error. |
SNMP PDUs had tooBig error-status |
Number of PDUs with a TooBig error (the maximum packet size is 1500 bytes). |
MIB objects retrieved successfully |
Number of MIB objects that have been successfully retrieved. |
MIB objects altered successfully |
Number of MIB objects that have been successfully modified. |
GetRequest-PDU accepted and processed |
Number of GetRequest requests that have been received and processed. |
GetNextRequest-PDU accepted and processed |
Number of getNext requests that have been received and processed. |
GetBulkRequest-PDU accepted and processed |
Number of getBulk requests that have been received and processed. |
GetResponse-PDU accepted and processed |
Number of get responses that have been received and processed. |
SetRequest-PDU accepted and processed |
Number of set requests that have been received and processed. |
Trap PDUs accepted and processed |
Number of notifications that have been received and processed. |
alternate Response Class PDUs dropped silently |
Number of dropped response packets. |
forwarded Confirmed Class PDUs dropped silently |
Number of forwarded packets that have been dropped. |
display snmp-agent sys-info
Use display snmp-agent sys-info to display SNMP agent system information.
display snmp-agent sys-info [ contact | location | version ] *
contact: Displays the system contact.
location: Displays the physical location of the device.
version: Displays the SNMP agent version.
If you do not specify any keywords, this command displays all SNMP agent system information.
# Display all SNMP agent system information.
<Sysname> display snmp-agent sys-info
The contact information of the agent:
New H3C Technologies Co., Ltd.
The location information of the agent:
Hangzhou, China
The SNMP version of the agent:
SNMPv3
snmp-agent sys-info
display snmp-agent trap queue
Use display snmp-agent trap queue to display basic information about the trap queue.
# Display the trap queue configuration and usage status.
<Sysname> display snmp-agent trap queue
Queue size: 100
Message number: 6
snmp-agent trap life
snmp-agent trap queue-size
display snmp-agent trap-list
Use display snmp-agent trap-list to display SNMP notifications enabling status for modules.
If a module has multiple sub-modules and SNMP notifications are enabled for one of its sub-modules, the command output shows that the module is SNMP notifications-enabled.
To determine whether a module supports SNMP notifications, execute the snmp-agent trap enable ? command.
The display snmp-agent trap-list command output varies by the snmp-agent trap enable command configuration and the module configuration.
# Display SNMP notifications enabling status for modules.
<Sysname> display snmp-agent trap-list
arp notification is disabled.
configuration notification is enabled.
mac-address notification is enabled.
radius notification is disabled.
standard notification is enabled.
syslog notification is disabled.
system notification is enabled.
Enabled notifications: 4; Disabled notifications: 3
display snmp-agent usm-user
Use display snmp-agent usm-user to display SNMPv3 user information.
display snmp-agent usm-user [ engineid engineid | group group-name | username user-name ] *
engineid engineid: Specifies an SNMP engine ID. The engine ID is case insensitive. When an SNMPv3 user is created, the system records the local SNMP entity engine ID. The user becomes invalid when the engine ID changes, and it becomes valid again when the recorded engine ID is restored.
group group-name: Specifies an SNMP group by its name. The group name is case sensitive.
username user-name: Specifies an SNMPv3 user by its name. The username is case sensitive.
This command displays only SNMPv3 users that you have created by using the snmp-agent usm-user v3 command. To display SNMPv1 or SNMPv2c users created by using the snmp-agent usm-user { v1 | v2c } command, use the display snmp-agent community command.
# Display information about all SNMPv3 users.
<Sysname> display snmp-agent usm-user
Username: userv3
Group name: mygroupv3
Engine ID: 800063A203000FE240A1A6
UserStatus: active
ACL: 2000
Username: userv3
Engine ID: 8000259503000BB3100A508
UserStatus: active
ACL name: testacl
Username: userv3code
Role name: groupv3code
UserStatus: active
Role name: snmprole
Engine ID: 800063A280000002BB0001
UserStatus: active
Table 11 Command output
Username |
SNMP username. |
Group name |
SNMP group name. |
Role name |
SNMP user role name. |
Engine ID |
Engine ID that the SNMP agent used when the SNMP user was created. |
Storage-type |
Storage type: · volatile. · nonvolatile. · permanent. · readOnly. · other. For more information about these storage types, see Table 1. |
UserStatus |
SNMP user status: · active—The SNMP user is effective. · notInService—The SNMP user is correctly configured but not activated. · notReady—The SNMP user configuration is incomplete. · other—Any other status. |
ACL |
Number of the ACL. This field appears only when an ACL is specified for the SNMPv3 user. It is exclusive with the ACL name field. |
ACL name |
Name of the ACL. This field appears only when an ACL is specified for the SNMPv3 user. It is exclusive with the ACL field. |
enable snmp trap updown
Use enable snmp trap updown to enable link state notifications on an interface.
Use undo enable snmp trap updown to disable link state notifications on an interface.
Link state notifications are enabled.
Interface view
For an interface to generate linkUp/linkDown notifications when its state changes, you must also enable the linkUp/linkDown notification function globally by using the snmp-agent trap enable standard [ linkdown | linkup ] * command.
# Enable GigabitEthernet 1/0/1 to send linkUp/linkDown SNMP traps to 10.1.1.1 in the community public.
[Sysname] snmp-agent target-host trap address udp-domain 10.1.1.1 params securityname public
[Sysname-GigabitEthernet1/0/1] enable snmp trap updown
snmp-agent
Use snmp-agent to enable the SNMP agent.
Use undo snmp-agent to disable the SNMP agent.
snmp-agent
undo snmp-agent
The SNMP agent is disabled.
The SNMP agent is automatically enabled when you execute any command that begins with snmp-agent except for the snmp-agent calculate-password command.
# Enable the SNMP agent.
Use snmp-agent { inform | trap } source to specify a source IP address for the informs or traps sent by the SNMP agent.
Use undo snmp-agent { inform | trap } source to restore the default.
snmp-agent { inform | trap } source interface-type { interface-number | interface-number.subnumber }
The SNMP agent uses the IP address of the outgoing interface as the source IP address of notifications.
inform: Specifies informs.
trap: Specifies traps.
interface-type { interface-number | interface-number.subnumber }: Specifies an interface by its type and number. The interface-number argument specifies a main interface number. The subnumber argument specifies a subinterface number in the range of 1 to 4094.
The snmp-agent source command enables the SNMP agent to use the primary IP address of an interface or subinterface as the source IP address in all its SNMP informs or traps, regardless of their outgoing interfaces. An NMS can use this IP address to filter all the informs or traps sent by the SNMP agent.
Make sure the specified interface has been created and assigned a valid IP address. The configuration will fail if the interface has not been created and will take effect only after a valid IP address is assigned to the specified interface.
# Configure the primary IP address of GigabitEthernet 1/0/1 as the source address of SNMP traps.
[Sysname] snmp-agent trap source gigabitethernet 1/0/1
# Configure the primary IP address of GigabitEthernet 1/0/2 as the source address of SNMP informs.
[Sysname] snmp-agent inform source gigabitethernet 1/0/2
Use snmp-agent calculate-password to calculate the encrypted form for a key in plaintext form.
In non-FIPS mode:
snmp-agent calculate-password plain-password mode { 3desmd5 | 3dessha | aes192md5 | aes192sha | aes256md5 | aes256sha | md5 | sha } { local-engineid | specified-engineid engineid }
In FIPS mode:
snmp-agent calculate-password plain-password mode { aes192sha | aes256sha | sha } { local-engineid | specified-engineid engineid }
plain-password: Specifies a key in plaintext form. The plain-password argument is a case-sensitive string of 1 to 64 characters.
mode: Specifies an authentication algorithm and encryption algorithm. The device supports the HMAC-MD5 and HMAC-SHA1 authentication algorithms. The HMAC-MD5 algorithm is faster than the HMAC-SHA1 algorithm. The HMAC-SHA1 algorithm provides more security than the HMAC-MD5 algorithm. The AES256, AES192, AES, 3DES, and DES encryption algorithms (in descending order of security strength) are available for the device. A more secure algorithm calculates slower. DES is enough to meet general security requirements.
· 3desmd5: Calculates the encrypted form for the encryption key by using the 3DES encryption algorithm and HMAC-MD5 authentication algorithm.
· 3dessha: Calculates the encrypted form for the encryption key by using the 3DES encryption algorithm and HMAC-SHA1 authentication algorithm.
· aes192md5: Calculates the encrypted form for the encryption key by using the AES192 encryption algorithm and the HMAC-MD5 authentication algorithm.
· aes192sha: Calculates the encrypted form for the encryption key by using the AES192 encryption algorithm and the HMAC-SHA1 authentication algorithm.
· aes256md5: Calculates the encrypted form for the encryption key by using the AES256 encryption algorithm and the HMAC-MD5 authentication algorithm.
· aes256 sha: Calculates the encrypted form for the encryption key by using the AES256 encryption algorithm and the HMAC-SHA1 authentication algorithm.
· md5: Calculates the encrypted form for the authentication key or encryption key by using the HMAC-MD5 authentication algorithm and AES or DES encryption algorithm. When the HMAC-MD5 authentication algorithm is used, you can get the same authentication key or encryption key in encrypted form regardless of whether the AES or DES encryption algorithm is used.
· sha: Calculates the encrypted form for the authentication key or encryption key by using HMAC-SHA1 authentication algorithm and AES or DES encryption algorithm. When the HMAC-SHA1 authentication algorithm is used, you can get the same authentication key or encryption key in encrypted form regardless of whether the AES or DES encryption algorithm is used.
local-engineid: Uses the local engine ID to calculate the encrypted form for the key. You can configure the local engine ID by using the snmp-agent local-engineid command.
specified-engineid engineid: Uses a user-defined engine ID to calculate the encrypted form for the key. The engineid argument is an even number of case-insensitive hexadecimal characters. All-zero and all-F strings are invalid. The even number is in the range of 10 to 64.
Make sure the SNMP agent is enabled before you execute the snmp-agent calculate-password command.
For security purposes, use the encrypted-form key generated by using this command when you create SNMPv3 users by specifying the cipher keyword in the snmp-agent usm-user v3 command.
The encrypted form of the key is valid only under the engine ID specified for key conversion.
# Use the local engine ID and the HMAC-SHA1 algorithm to calculate the encrypted form for key authkey.
[Sysname] snmp-agent calculate-password authkey mode sha local-engineid
The encrypted key is: 09659EC5A9AE91BA189E5845E1DDE0CC
Use snmp-agent community to configure an SNMPv1 or SNMPv2c community.
Use undo snmp-agent community to delete an SNMPv1 or SNMPv2c community.
In VACM mode:
snmp-agent community { read | write } [ simple | cipher ] community-name [ mib-view view-name ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
undo snmp-agent community [ cipher ] community-name
In RBAC mode:
snmp-agent community [ simple | cipher ] community-name user-role role-name [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
No SNMPv1 or SNMPv2c communities exist.
read: Assigns the specified community read-only access to MIB objects. A read-only community can only inquire MIB information.
write: Assigns the specified community read and write access to MIB objects. A read and write community can configure MIB information.
simple: Specifies a community name in plaintext form. For security purposes, the community name specified in plaintext form will be stored in encrypted form.
cipher: Specifies a community name in encrypted form.
community-name: Specifies the community name. The plaintext form is a case-sensitive string of 1 to 32 characters. The encrypted form is a case-sensitive string of 33 to 73 characters. Input a string as escape characters after a backslash (\).
mib-view view-name: Specifies the MIB view available for the community. The view-name argument represents a MIB view name, a case-sensitive string of 1 to 32 characters. A MIB view represents a set of accessible MIB objects. If you do not specify a view, the specified community can access the MIB objects in the default MIB view ViewDefault.
user-role role-name: Specifies a user role name for the community, a case-sensitive string of 1 to 63 characters.
acl: Specifies a basic or advanced IPv4 ACL for the community.
ipv4-acl-number: Specifies a basic or advanced IPv4 ACL by its number. The basic IPv4 ACL number is in the range of 2000 to 2999. The advanced IPv4 ACL number is in the range of 3000 to 3999.
name ipv4-acl-name: Specifies a basic or advanced IPv4 ACL by its name, a case-insensitive string of 1 to 63 characters.
acl ipv6: Specifies a basic or advanced IPv6 ACL for the community.
ipv6-acl-number: Specifies a basic or advanced IPv6 ACL by its number. The basic IPv6 ACL number is in the range of 2000 to 2999. The advanced IPv6 ACL number is in the range of 3000 to 3999.
name ipv6-acl-name: Specifies a basic or advanced IPv6 ACL by its name, a case-insensitive string of 1 to 63 characters.
Only users with the network-admin or level-15 user role can execute this command. Users with other user roles cannot execute this command even if these roles are granted access to commands of the SNMP feature or this command.
An SNMP community is identified by a community name. It contains a set of NMSs and SNMP agents. Devices in an SNMP community authenticate each other by using the community name. An NMS and an SNMP agent can communicate only when they use the same community name.
Typically, public is used as the read-only community name and private is used as the read and write community name. To enhance security, you can assign your SNMP communities a name other than public and private.
The snmp-agent community command allows you to use either of the following modes to control SNMP community access to MIB objects:
· View-based access control model—The VACM mode controls access to MIB objects by assigning MIB views to SNMP communities.
· Role based access control—The RBAC mode controls access to MIB objects by assigning user roles to SNMP communities.
¡ The network-admin and level-15 user roles have the read and write access to all MIB objects.
¡ The network-operator user role have the read-only access to all MIB objects.
For more information about user roles, see Fundamentals Configuration Guide.
RBAC mode controls access on a per MIB object basis, and VACM mode controls access on a MIB view basis. As a best practice to enhance MIB security, use RBAC mode.
You can create a maximum of 10 SNMP communities by using the snmp-agent community command.
If you execute the command multiple times to specify the same community name but different other settings each time, the most recent configuration takes effect.
To set and save a community name in plain text, do not specify the simple or cipher keyword.
The ACL is used to filter illegitimate NMSs.
· If you do not specify an ACL, the specified ACL does not exist, or the specified ACL does not have any rules, all NMSs that use the community name can access the SNMP agent.
· If you specify an ACL and the ACL has rules, only NMSs permitted by the ACL can access the SNMP agent.
For more information about ACL, see ACL and QoS Configuration Guide.
You can also create an SNMP community by using the snmp-agent usm-user { v1 | v2c } and snmp-agent group { v1 | v2c } commands. These two commands create an SNMPv1 or SNMPv2c user and the group to which the user is assigned. The system automatically creates an SNMP community by using the SNMPv1 or SNMPv2c username.
# Create the read-only community with the plaintext form name readaccess so an SNMPv1 or SNMPv2c NMS can use the community name readaccess to read the MIB objects in the default view ViewDefault.
[Sysname] snmp-agent sys-info version v1 v2c
[Sysname] snmp-agent community read simple readaccess
# Create the read and write community with the plaintext form name writeaccess so only the SNMPv2c NMS at 1.1.1.1 can use the community name writeaccess to read or set the MIB objects in the default view ViewDefault.
[Sysname] acl basic 2001
[Sysname-acl-ipv4-basic-2001] rule permit source 1.1.1.1 0.0.0.0
[Sysname-acl-ipv4-basic-2001] rule deny source any
[Sysname] snmp-agent sys-info version v2c
[Sysname] snmp-agent community write simple writeaccess acl 2001
# Create the read and write community with the plaintext form name writeaccess so only the SNMPv2c NMS at 1.1.1.2 can use the community name writeaccess to read or set the MIB objects in the default view ViewDefault.
[Sysname] acl basic name testacl
[Sysname-acl-ipv4-basic-testacl] rule permit source 1.1.1.2 0.0.0.0
[Sysname-acl-ipv4-basic-testacl] rule deny source any
[Sysname-acl-ipv4-basic-testacl] quit
[Sysname] snmp-agent community write simple writeaccess acl name testacl
# Create the read and write community with the plaintext form name wr-sys-acc so an SNMPv1 or SNMPv2c NMS can use the community name wr-sys-acc to read or set the MIB objects in the system subtree (OID 1.3.6.1.2.1.1).
[Sysname] undo snmp-agent mib-view ViewDefault
[Sysname] snmp-agent mib-view included test system
[Sysname] snmp-agent community write simple wr-sys-acc mib-view test
snmp-agent mib-view
snmp-agent community-map
Use snmp-agent community-map to map an SNMP community to an SNMP context.
Use undo snmp-agent community-map to delete the mapping between an SNMP community and an SNMP context.
snmp-agent community-map community-name context context-name
undo snmp-agent community-map community-name context context-name
No mapping exists between an SNMP community and an SNMP context.
community-name: Specifies an SNMP community, a case-sensitive string of 1 to 32 characters.
context-name: Specifies an SNMP context, a case-sensitive string of 1 to 32 characters.
This command enables a module on an agent to obtain the context mapped to a community name when an NMS accesses the agent by using SNMPv1 or SNMPv2c.
You can configure a maximum of 10 community-context mappings on the device.
# Map SNMP community private to SNMP context trillcontext.
[Sysname] snmp-agent community-map private context testcontext
snmp-agent context
Use snmp-agent context to create an SNMP context.
Use undo snmp-agent context to delete an SNMP context.
snmp-agent context context-name
undo snmp-agent context context-name
No SNMP contexts exist.
Predefined use roles
For an NMS and an SNMP agent to communicate, configure the same SNMP context for them or do not configure a context for the NMS.
You can create a maximum of 20 SNMP contexts.
# Create SNMP context trillcontext.
[Sysname] snmp-agent context testcontext
snmp-agent group
Use snmp-agent group to create an SNMP group.
Use undo snmp-agent group to delete an SNMP group.
SNMPv1 and SNMPv2c:
snmp-agent group { v1 | v2c } group-name [ read-view view-name ] [ write-view view-name ] [ notify-view view-name ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
undo snmp-agent group { v1 | v2c } group-name
SNMPv3:
In non-FIPS mode:
snmp-agent group v3 group-name [ authentication | privacy ] [ read-view read-view ] [ write-view write-view ] [ notify-view notify-view ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
undo snmp-agent group v3 group-name [ authentication | privacy ]
In FIPS mode:
snmp-agent group v3 group-name { authentication | privacy } [ read-view read-view ] [ write-view write-view ] [ notify-view notify-view ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
undo snmp-agent group v3 group-name { authentication | privacy }
No SNMP groups exist.
v1: Specifies SNMPv1.
v2c: Specifies SNMPv2c.
v3: Specifies SNMPv3.
group-name: Specifies an SNMP group name, a case-sensitive string of 1 to 32 characters.
authentication: Specifies the authentication without privacy security model for the SNMPv3 group.
privacy: Specifies the authentication with privacy security model for the SNMPv3 group.
read-view view-name: Specifies a read-only MIB view. The view-name represents a MIB view name, a case-sensitive string of 1 to 32 characters. If you do not specify a read-only MIB view, the SNMP group has read access to the default view ViewDefault.
write-view view-name: Specifies a read and write MIB view. The view-name represents a MIB view name, a case-sensitive string of 1 to 32 characters. If you do not specify a read and write view, the SNMP group cannot set any MIB object on the SNMP agent.
notify-view view-name: Specifies a notify MIB view. The view-name represents a MIB view name, a case-sensitive string of 1 to 32 characters. The SNMP agent sends notifications to the users in the specified group only for the MIB objects included in the notify view. If you do not specify a notify view, the SNMP agent does not send any notification to the users in the specified group.
acl: Specifies a basic or advanced IPv4 ACL for the group.
acl ipv6: Specifies a basic or advanced IPv6 ACL for the group.
SNMPv1 and SNMPv2c settings in this command are not supported in FIPS mode.
All users in an SNMP group share the security model and access rights of the group.
You can create a maximum of 20 SNMP groups, including SNMPv1, SNMPv2c, and SNMPv3 groups.
All SNMPv3 users in a group share the same security model, but can use different authentication and encryption key settings. To implement a security model for a user and avoid SNMP communication failures, make sure the security model configuration for the group and the security key settings for the user are compliant with Table 12 and match the settings on the NMS.
Table 12 Basic security setting requirements for different security models
Security model |
Security model keyword for the group |
Security key settings for the user |
Remarks |
Authentication with privacy |
privacy |
Authentication key, encryption key |
If the authentication key or the encryption key is not configured, SNMP communication will fail. |
Authentication without privacy |
authentication |
Authentication key |
If no authentication key is configured, SNMP communication will fail. The encryption key (if any) for the user does not take effect. |
No authentication, no privacy |
Neither authentication nor privacy |
None |
The authentication and encryption keys, if configured, do not take effect. |
You can specify an ACL for the user and group, respectively, to filter illegitimate NMSs. Only the NMSs permitted by the ACLs for both the user and group can access the SNMP agent. The following rules apply to the ACLs for the user and group:
· If you do not specify an ACL, the specified ACL does not exist, or the specified ACL does not have any rules, all NMSs that use the username can access the SNMP agent.
· If you have specified an ACL and the ACL has rules, only the NMSs permitted by the ACL can access the agent.
# Create the SNMPv3 group group1.
[Sysname] snmp-agent group v3 group1
snmp-agent mib-view
snmp-agent usm-user
Use snmp-agent local-engineid to set an SNMP engine ID.
Use undo snmp-agent local-engineid to restore the default.
The engine ID of a device is the combination of the company ID and the device ID. The device ID varies by device model.
engineid: Specifies an SNMP engine ID, a case-insensitive hexadecimal string. Its length is an even number in the range of 10 to 64. All-zero and all-F strings are invalid.
An SNMP engine ID uniquely identifies a device in an SNMP managed network. Make sure the local SNMP engine ID is unique within your SNMP managed network to avoid communication problems.
If you have configured SNMPv3 users, change the local SNMP engine ID only when necessary. The change can void the SNMPv3 usernames and encrypted keys you have configured.
You can use the default engine ID or configure an easy-to-remember engine ID based on the network plan. For example, you can set the engine ID for device 1 on the first floor of building A to 000Af0010001 and device 2 to 000Af0010002.
# Set the local SNMP engine ID to 123456789A.
[Sysname] snmp-agent local-engineid 123456789A
snmp-agent usm-user
snmp-agent log
Use snmp-agent log to enable SNMP logging.
Use undo snmp-agent log to disable SNMP logging.
snmp-agent log { all | authfail | get-operation | set-operation }
undo snmp-agent log { all | authfail | get-operation | set-operation }
SNMP logging operations are disabled.
all: Enables logging SNMP authentication failures, Get operations, and Set operations.
authfail: Enables logging SNMP authentication failures.
get-operation: Enables logging SNMP Get operations.
set-operation: Enables logging SNMP Set operations.
Use SNMP logging to record the SNMP operations performed on the SNMP agent or authentication failures from the NMS to the agent for auditing NMS behaviors. The SNMP agent sends log data to the information center. You can configure the information center to output the data to a destination as needed.
# Enable logging SNMP Get operations.
[Sysname] snmp-agent log get-operation
# Enable logging SNMP Set operations.
[Sysname] snmp-agent log set-operation
# Enable logging SNMP authentication failures.
[Sysname] snmp-agent log authfail
snmp-agent mib-view
Use snmp-agent mib-view to create or update a MIB view.
Use undo snmp-agent mib-view to delete a MIB view.
undo snmp-agent mib-view view-name
The system creates the ViewDefault view when the SNMP agent is enabled. In this default MIB view, all MIB objects in the iso subtree but the snmpUsmMIB, snmpVacmMIB, and snmpModules.18 subtrees are accessible.
excluded: Denies access to any node in the specified MIB subtree.
included: Permits access to all the nodes in the specified MIB subtree.
view-name: Specifies a view name, a case-sensitive string of 1 to 32 characters.
oid-tree: Specifies a MIB subtree by its root node's OID (for example, 1.3.6.1.2.1.1) or object name (for example, system). The oid-tree argument is a case-sensitive string of 1 to 255 characters. An OID is a dotted numeric string that uniquely identifies an object in the MIB tree.
mask mask-value: Sets a MIB subtree mask, a case-insensitive hexadecimal string. Its length is an even number in the range of 1 to 32.
A MIB view represents a set of MIB objects (or MIB object hierarchies) with certain access privilege. The MIB objects included in the MIB view are accessible while those excluded from the MIB view are inaccessible.
Each view-name oid-tree pair represents a view record. If you specify the same record with different MIB subtree masks multiple times, the most recent configuration takes effect.
Be cautious with deleting the default MIB view. The operation blocks the access to any MIB object on the device from NMSs that use the default view.
# Include the mib-2 (OID 1.3.6.1.2.1) subtree in the mibtest view and exclude the system subtree from this view.
[Sysname] snmp-agent mib-view included mibtest 1.3.6.1.2.1
[Sysname] snmp-agent mib-view excluded mibtest system
[Sysname] snmp-agent community read public mib-view mibtest
An SNMPv1 NMS in the public community can query the objects in the mib-2 subtree but not any object (for example, the sysDescr or sysObjectID node) in the system subtree.
snmp-agent group
snmp-agent packet max-size
Use snmp-agent packet max-size to set the maximum size (in bytes) of SNMP packets that the SNMP agent can receive or send.
Use undo snmp-agent packet max-size to restore the default.
An SNMP agent can process SNMP packets with a maximum size of 1500 bytes.
byte-count: Sets the maximum size (in bytes) of SNMP packets that the SNMP agent can receive or send. The value range is 484 to 17940.
If any device on the path to the NMS does not support packet fragmentation, limit the SNMP packet size to prevent large-sized packets from being discarded. For most networks, the default value is sufficient.
# Set the maximum SNMP packet size to 1024 bytes.
[Sysname] snmp-agent packet max-size 1024
snmp-agent port
Use snmp-agent port to specify the UDP port for receiving SNMP packets.
Use undo snmp-agent port to restore the default.
snmp-agent port port-num
The device uses UDP port 161 for receiving SNMP packets.
port-num: Specifies the UDP port for receiving SNMP packets, in the range of 1 to 65535. The default port number is 161.
After changing the port number for receiving SNMP packets, reconnect the device by using the port number for SNMP get and set operations.
To display UDP port information, use the display current-configuration command.
# Specify the UDP port for receiving SNMP packets as 5555.
[Sysname] snmp-agent port 5555
# Restore the default UDP port.
[Sysname] undo snmp-agent port
snmp-agent remote
Use snmp-agent remote to set an SNMP engine ID for a remote SNMP entity.
Use undo snmp-agent remote to delete the SNMP engine ID of a remote SNMP entity.
snmp-agent remote { ipv4-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ] engineid engineid
undo snmp-agent remote ip-address
No SNMP engine IDs are configured for remote SNMP entities.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the remote SNMP entity belongs. The vpn-instance-name argument represents the VPN instance name. a case-sensitive string of 1 to 31 characters. If the SNMP entity belongs to the public network, do not specify this option.
engineid: Specifies the SNMP engine ID of the remote SNMP entity. This argument is a case-insensitive hexadecimal string. Its length is an even number in the range of 10 to 64. All-zero and all-F strings are invalid.
To send informs to an NMS, you must configure the SNMP engine ID of the NMS on the SNMP agent.
The NMS accepts the SNMPv3 informs from the SNMP agent only if the engine ID in the informs is the same as its local engine ID.
You can configure a maximum of 20 remote SNMP engine IDs.
# Set the SNMP engine ID to 123456789A for the remote entity 10.1.1.1.
[Sysname] snmp-agent remote 10.1.1.1 engineid 123456789A
snmp-agent sys-info contact
Use snmp-agent sys-info contact to configure the system contact.
Use undo snmp-agent sys-info contact to restore the default contact.
snmp-agent sys-info contact sys-contact
The system contact is New H3C Technologies Co., Ltd..
sys-contact: Specifies the system contact, a case-sensitive string of 1 to 255 characters.
Configure the system contact for system maintenance and management.
# Configure the system contact as Dial System Operator # 27345.
[Sysname] snmp-agent sys-info contact Dial System Operator # 27345
snmp-agent sys-info location
Use snmp-agent sys-info location to configure the system location.
Use undo snmp-agent sys-info location to restore the default location.
snmp-agent sys-info location sys-location
The system location is Hangzhou, China.
sys-location: Specifies the system location, a case-sensitive string of 1 to 255 characters.
Configure the location of the device for system maintenance and management.
# Configure the system location as Room524-row1-3.
[Sysname] snmp-agent sys-info location Room524-row1-3
Use snmp-agent sys-info version to enable SNMP versions.
Use undo snmp-agent sys-info version to disable SNMP versions.
In non-FIPS mode:
snmp-agent sys-info version { all | { v1 | v2c | v3 } * }
undo snmp-agent sys-info version { all | { v1 | v2c | v3 } * }
In FIPS mode:
snmp-agent sys-info version v3
undo snmp-agent sys-info version v3
SNMPv3 is enabled.
all: Specifies SNMPv1, SNMPv2c, and SNMPv3.
Configure the SNMP agent with the same SNMP version as the NMS for successful communications between them.
# Enable SNMPv3.
[Sysname] snmp-agent sys-info version v3
Use snmp-agent target-host to configure an SNMP notification target host.
Use undo snmp-agent target-host to remove an SNMP notification target host.
In non-FIPS mode:
snmp-agent target-host inform address udp-domain { ipv4-address | ipv6 ipv6-address } [ udp-port port-number ] [ vpn-instance vpn-instance-name ] params securityname security-string { v2c | v3 [ authentication | privacy ] }
snmp-agent target-host trap address udp-domain { ipv4-address | ipv6 ipv6-address } [ udp-port port-number ] [ vpn-instance vpn-instance-name ] params securityname security-string [ v1 | v2c | v3 [ authentication | privacy ] ]
undo snmp-agent target-host { trap | inform } address udp-domain { ipv4-address | ipv6 ipv6-address } params securityname security-string [ vpn-instance vpn-instance-name ]
In FIPS mode:
snmp-agent target-host inform address udp-domain { ipv4-address | ipv6 ipv6-address } [ udp-port port-number ] [ vpn-instance vpn-instance-name ] params securityname security-string v3 { authentication | privacy }
snmp-agent target-host trap address udp-domain { ipv4-address | ipv6 ipv6-address } [ udp-port port-number ] [ vpn-instance vpn-instance-name ] params securityname security-string v3 { authentication | privacy }
No SNMP notification target hosts exist.
inform: Specifies a host that receives informs.
trap: Specifies a host that receives traps.
address: Specifies the destination address of SNMP notifications.
udp-domain: Specifies UDP as the transport protocol.
ipv4-address: Specifies a target host by its IPv4 address or host name. The host name is a case-insensitive string of 1 to 253 characters. The string can only contain letters, numbers, hyphens (-), underscores (_), and dots (.). If you specify a host name, the IPv4 address of the target host can be obtained.
ipv6 ipv6-address: Specifies a target host by its IPv6 address or host name. The host name is a case-insensitive string of 1 to 253 characters, which only contains letters, numbers, hyphens (-), underscores (_), and dots (.). If you specify a host name, the IPv6 address of the target host can be obtained. If you specify an IPv6 address, the address cannot be a link local address.
udp-port port-number: Specifies the UDP port for SNMP notifications. The default port number is 162.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the target host belongs. The vpn-instance-name argument represents the VPN instance name, a case-sensitive string of 1 to 31 characters. If the target host belongs to the public network, do not specify this option.
params securityname security-string: Specifies the authentication parameter. The security-string argument specifies an SNMPv1 or SNMPv2c community name or an SNMPv3 username, a case-sensitive string of 1 to 32 characters.
· authentication: Specifies the security model to be authentication without privacy. You must specify the authentication key when you create the SNMPv3 user.
· privacy: Specifies the security model to be authentication with privacy. You must specify the authentication key and encryption key when you create the SNMPv3 user.
You can specify multiple SNMP notification target hosts.
Make sure the SNMP agent uses the same UDP port for SNMP notifications as the target host. Typically, NMSs, for example, IMC and MIB Browser, use port 162 for SNMP notifications as defined in the SNMP protocols.
If none of the keywords v1, v2c, or v3 is specified, SNMPv1 is used. Make sure the SNMP agent uses the same SNMP version as the target host so the host can receive the notification.
If neither authentication nor privacy is specified, the security model is no authentication, no privacy.
# Configure the SNMP agent to send SNMPv3 traps to 10.1.1.1 by using the username public.
[Sysname] snmp-agent trap enable standard
[Sysname] snmp-agent target-host trap address udp-domain 10.1.1.1 params securityname public v3
Use snmp-agent trap enable to enable SNMP notifications.
Use undo snmp-agent trap enable to disable SNMP notifications.
snmp-agent trap enable [ configuration | protocol | standard [ authentication | coldstart | linkdown | linkup | warmstart ] * | system ]
undo snmp-agent trap enable [ configuration | protocol | standard [ authentication | coldstart | linkdown | linkup | warmstart ] * | system ]
SNMP configuration notifications, standard notifications, and system notifications are enabled. Whether other SNMP notifications are enabled varies by module.
configuration: Specifies configuration notifications. If configuration notifications are enabled, the system checks the running configuration and the startup configuration every 10 minutes for any change and generates a notification for the most recent change.
protocol: Specifies protocol module notifications. You can use the snmp-agent trap enable ? command to obtain the value of this argument. For more information about this argument, see the command reference for each module.
standard: Specifies SNMP standard notifications.
Table 13 Standard SNMP notifications
Keyword |
Definition |
authentication |
Authentication failure notification sent when an NMS fails to be authenticated by the SNMP agent. |
coldstart |
Notification sent when the device restarts. |
linkdown |
Notification sent when the link of a port goes down. |
linkup |
Notification sent when the link of a port comes up. |
warmstart |
Notification sent when the SNMP agent restarts. |
system: Specifies system notifications sent when the system time is modified, the system reboots, or the main system software image is not available.
To report critical protocol events to an NMS, enable SNMP notifications for the protocol. For SNMP notifications to be sent correctly, you must also configure the notification sending parameters as required.
If no optional parameters are specified, this command or its undo form enables or disables all SNMP notifications supported by the device.
# Enable the SNMP agent to send SNMP authentication failure notifications.
[Sysname] snmp-agent trap enable standard authentication
Use snmp-agent trap if-mib link extended to configure the SNMP agent to send extended linkUp/linkDown notifications.
Use undo snmp-agent trap if-mib link extended to restore the default.
The SNMP agent sends standard linkUp/linkDown notifications.
Extended linkUp and linkDown notifications add interface description and interface type to the standard linkUp/linkDown notifications for fast failure point identification.
When you use this command, make sure the NMS supports the extended linkup and linkDown notifications.
# Enable extended linkUp/linkDown notifications.
[Sysname] snmp-agent trap if-mib link extended
Use snmp-agent trap life to set the lifetime of notifications in the SNMP notification queue.
Use undo snmp-agent trap life to restore the default notification lifetime.
snmp-agent trap life seconds
The SNMP notification lifetime is 120 seconds.
seconds: Sets a lifetime in the range of 1 to 2592000, in seconds.
When congestion occurs, the SNMP agent buffers notifications in a queue. The notification lifetime sets how long a notification can stay in the queue. A notification is deleted when its lifetime expires.
# Set the SNMP notification lifetime to 60 seconds.
[Sysname] snmp-agent trap life 60
snmp-agent trap log
Use snmp-agent trap log to enable SNMP notification logging.
Use undo snmp-agent trap log to disable SNMP notification logging.
snmp-agent trap log
SNMP notification logging is disabled.
Use SNMP notification logging to record SNMP notifications sent by the SNMP agent for notification tracking. The SNMP agent sends the logs to the information center. You can configure the information center to output the logs to a destination as needed.
# Enable SNMP notification logging.
[Sysname] snmp-agent trap log
Use snmp-agent trap queue-size to set the SNMP notification queue size.
Use undo snmp-agent trap queue-size to restore the default queue size.
The SNMP notification queue can store a maximum of 100 notifications.
size: Specifies the maximum number of notifications that the SNMP notification queue can hold. The value range is 1 to 1000.
When congestion occurs, the SNMP agent buffers notifications in a queue. SNMP notification queue size sets the maximum number of notifications that this queue can hold. When the queue size is reached, the oldest notifications are dropped for new notifications.
# Set the SNMP notification queue size to 200.
[Sysname] snmp-agent trap queue-size 200
Use snmp-agent usm-user { v1 | v2c } to create an SNMPv1 or SNMPv2c user.
Use undo snmp-agent usm-user { v1 | v2c } to delete an SNMPv1 or SNMPv2c user.
snmp-agent usm-user { v1 | v2c } user-name group-name [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
undo snmp-agent usm-user { v1 | v2c } user-name
No SNMPv1 or SNMPv2c users exist.
user-name: Specifies an SNMP username, a case-sensitive string of 1 to 32 characters.
group-name: Specifies an SNMPv1 or SNMPv2c group name, a case-sensitive string of 1 to 32 characters. The group can be one that has been created or not. The user takes effect only after you create the group.
acl: Specifies a basic or advanced IPv4 ACL for the user.
acl ipv6: Specifies a basic or advanced IPv6 ACL for the user.
This command is not available in FIPS mode.
On an SNMPv1 or SNMPv2c network, NMSs and agents authenticate each other by using the community name. On an SNMPv3 network, NMSs and agents authenticate each other by using the username.
You can create an SNMPv1 or SNMPv2c community by using either of the following ways:
· Execute the snmp-agent community command.
· Execute the snmp-agent usm-user { v1 | v2c } and snmp-agent group { v1 | v2c } commands to create an SNMPv1 or SNMPv2c user and the group that the user is assigned to. The system automatically creates an SNMP community by using the SNMPv1 or SNMPv2c username.
# Add the user userv2c to the SNMPv2c group readCom so an NMS can use the protocol SNMPv2c and the read-only community name userv2c to access the device.
[Sysname] snmp-agent group v2c readCom
[Sysname] snmp-agent usm-user v2c userv2c readCom
# Add the user userv2c in the SNMPv2c group readCom so only the NMS at 1.1.1.1 can use the protocol SNMPv2c and read-only community name userv2c to access the device.
[Sysname] snmp-agent usm-user v2c userv2c readCom acl 2001
# Add the user userv2c in the SNMPv2c group readCom so only the NMS at 1.1.1.2 can use the protocol SNMPv2c and read-only community name userv2c to access the device.
[Sysname] snmp-agent usm-user v2c userv2c readCom acl name testacl
snmp-agent group
Use snmp-agent usm-user v3 to create an SNMPv3 user.
Use undo snmp-agent usm-user v3 to delete an SNMPv3 user.
In non-FIPS mode:
· In VACM mode:
snmp-agent usm-user v3 user-name group-name [ remote { ipv4-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ] ] [ { cipher | simple } authentication-mode { md5 | sha } auth-password [ privacy-mode { 3des | aes128 | aes192 | aes256 | des56 } priv-password ] ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
undo snmp-agent usm-user v3 user-name { local | engineid engineid-string | remote { ipv4-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ] }
· In RBAC mode:
snmp-agent usm-user v3 user-name user-role role-name [ remote { ipv4-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ] ] [ { cipher | simple } authentication-mode { md5 | sha } auth-password [ privacy-mode { 3des | aes128 | aes192 | aes256 | des56 } priv-password ] ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
In FIPS mode:
· In VACM mode:
snmp-agent usm-user v3 user-name group-name [ remote { ipv4-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ] ] { cipher | simple } authentication-mode sha auth-password [ privacy-mode { aes128 | aes192 | aes256 } priv-password ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
· In RBAC mode:
snmp-agent usm-user v3 user-name user-role role-name [ remote { ipv4-address | ipv6 ipv6-address } [ vpn-instance vpn-instance-name ] ] [ { cipher | simple } authentication-mode sha auth-password [ privacy-mode { aes128 | aes192 | aes256 } priv-password ] ] [ acl { ipv4-acl-number | name ipv4-acl-name } | acl ipv6 { ipv6-acl-number | name ipv6-acl-name } ] *
No SNMPv3 users exist.
user-name: Specifies an SNMPv3 username, a case-sensitive string of 1 to 32 characters.
group-name: Specifies an SNMPv3 group name, a case-sensitive string of 1 to 32 characters. The group can be one that has been created or not. The user takes effect only after you create the group.
user-role role-name: Specifies a user role name, a case-sensitive string of 1 to 63 characters.
remote { ipv4-address | ipv6 ipv6-address }: Specifies a target host by its IPv4 or IPv6 address, typically the NMS, to receive the notifications. To send SNMPv3 notifications to a target host, you need to specify this option and use the snmp-agent remote command to bind the IPv4 or IPv6 address to the remote engine ID.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the target host belongs to. The vpn-instance-name argument represents the VPN instance name, a case-sensitive string of 1 to 31 characters. If the target host belongs to the public network, do not specify this option.
cipher: Specifies an authentication key and an encryption key in encrypted form. The keys will be converted to a digest in encrypted form and stored in the device.
simple: Specifies an authentication key and an encryption key in plaintext from. The keys will be converted to a digest in encrypted form and stored in the device.
authentication-mode: Specifies an authentication algorithm. If you do not specify the keyword, the system does not perform authentication. For more information about authentication algorithms, see IPSec configuration in Security Configuration Guide.
· md5: Specifies the HMAC-MD5 authentication algorithm.
· sha: Specifies the HMAC-SHA1 authentication algorithm.
auth-password: Specifies an authentication key. This argument is case sensitive.
· The plaintext form of the key in non-FIPS mode is a string of 1 to 64 characters. The plaintext form of the key in FIPS mode is a string of 15 to 64 characters, which must contain numbers, uppercase letters, lowercase letters, and special characters.
· The encrypted form of the key can be calculated by using the snmp-agent calculate-password command.
privacy-mode: Specifies an encryption algorithm. If you do not specify this keyword, the system does not perform encryption.
· 3des: Specifies the 3DES encryption algorithm that uses a 168-bit key.
· aes128: Specifies the AES encryption algorithm that uses a 128-bit key.
· aes192: Specifies the AES encryption algorithm that uses a 192-bit key.
· aes256: Specifies the AES encryption algorithm that uses a 256-bit key.
· des56: Specifies the DES encryption algorithm that uses a 56-bit key.
priv-password: Specifies an encryption key. This argument is case sensitive.
local: Specifies the local SNMP engine. By default, an SNMPv3 user is associated with the local SNMP engine.
engineid engineid-string: Specifies an SNMP engine ID. The engineid-string argument is an even number of hexadecimal characters. All-zero and all-F strings are invalid. The even number is in the range of 10 to 64. If you change the local engine ID, the existing SNMPv3 users and keys become invalid. To delete an invalid username, specify the engine ID associated with the username in the undo snmp-agent usm-user v3 command.
You can use either of the following modes to control SNMPv3 user access to MIB objects.
· VACM—Controls user access to MIB objects by assigning the user to an SNMP group. To make sure the user takes effect, make sure the group has been created. An SNMP group contains one or multiple users and specifies the MIB views and security model for the users. The authentication and encryption algorithms for each user are specified when they are created.
· RBAC—Controls user access to MIB objects by assigning user roles to the user. A user role specifies the MIB objects accessible to the user and the operations that the user can perform on the objects. After you create a user in RBAC mode, you can use the snmp-agent usm-user v3 user-role command to assign more user roles to the user. You can assign a maximum of 64 user roles to a user.
You can execute the snmp-agent usm-user v3 command multiple times to create different SNMPv3 users in VACM mode. If you do not change the username each time, the most recent configuration takes effect.
You can execute the snmp-agent usm-user v3 command in RBAC mode multiple times to assign different user roles to an SNMPv3 user. The following restrictions and guidelines apply:
· If you specify only user roles but do not change any other settings each time, the snmp-agent usm-user v3 command assigns different user roles to the user. Other settings remain unchanged.
· If you specify user roles and also change other settings each time, the snmp-agent usm-user v3 command assigns different user roles to the user. The most recent configuration for other settings takes effect.
You can specify an ACL for the user and group, respectively, to filter illegitimate NMSs from accessing the agent. Only the NMSs permitted by the ACLs for both the user and group can access the SNMP agent. The following rules apply to the ACLs for the user and group:
In VACM mode:
# Add user testUser to SNMPv3 group testGroup, and enable authentication for the group. Specify authentication algorithm HMAC-SHA1 and plaintext-form authentication key 123456TESTplat&! for the user.
[Sysname] snmp-agent group v3 testGroup authentication
[Sysname] snmp-agent usm-user v3 testUser testGroup simple authentication-mode sha 123456TESTplat&!
# For an NMS to access the MIB objects in the default view ViewDefault, make sure the following configurations on the NMS are the same as the SNMP agent:
· SNMPv3 username.
· SNMP protocol version.
· Authentication algorithm and key.
# Add user testUser to SNMPv3 group testGroup, and enable authentication and encryption for the group. Specify authentication algorithm HMAC-SHA1, encryption algorithm AES, plaintext-form authentication key 123456TESTauth&!, and plaintext-form encryption key 123456TESTencr&! for the user.
[Sysname] snmp-agent group v3 testGroup privacy
[Sysname] snmp-agent usm-user v3 testUser testGroup simple authentication-mode sha 123456TESTauth&! privacy-mode aes128 123456TESTencr&!
· SNMPv3 username.
· Authentication algorithm.
· Privacy algorithm.
· Plaintext authentication and encryption keys.
# Add user remoteUser for the SNMP remote engine at 10.1.1.1 to SNMPv3 group testGroup, and enable authentication and encryption for the group. Specify authentication algorithm HMAC-SHA1, encryption algorithm AES, plaintext-form authentication key 123456TESTauth&!, and plaintext-form encryption key 123456TESTencr&! for the user.
[Sysname] snmp-agent usm-user v3 remoteUser testGroup remote 10.1.1.1 simple authentication-mode sha 123456TESTauth&! privacy-mode aes128 123456TESTencr&!
In RBAC mode:
# Create SNMPv3 user testUser with user role network-operator and enable authentication for the user. Specify authentication algorithm HMAC-SHA1 and plaintext-form authentication key 123456TESTplat&! for the user.
[Sysname] snmp-agent usm-user v3 testUser user-role network-operator simple authentication-mode sha 123456TESTplat&!
For an NMS to have read-only access to all MIB objects, make sure the following configurations on the NMS are the same as the SNMP agent:
· SNMPv3 username.
snmp-agent group
snmp-agent remote
Use snmp-agent usm-user v3 user-role to assign a user role to an SNMPv3 user created in RBAC mode.
Use undo snmp-agent usm-user user-role to remove a user role.
undo snmp-agent usm-user v3 user-name user-role role-name
An SNMPv3 user has the user role assigned to it at its creation.
You can assign a maximum of 64 user roles to an SNMPv3 user.
An SNMPv3 user must have a minimum of one user role.
# Assign the user role network-admin to the SNMPv3 user testUser.
[Sysname] snmp-agent usm-user v3 testUser user-role network-admin