- 14-Network Management and Monitoring Command Reference
- 02-NQA commands
- 03-NTP commands
- 04-PTP commands
- 05-Network synchronization commands
- 06-SNMP commands
- 07-RMON commands
- 08-NETCONF commands
- 09-CWMP commands
- 10-EAA commands
- 11-Process monitoring and maintenance commands
- 12-Sampler commands
- 13-Mirroring commands
- 14-NetStream commands
- 15-IPv6 NetStream commands
- 16-Fast log output commands
- 17-Flow log commands
- 18-Information center commands
- 19-GOLD commands
- 20-Packet capture commands
- 21-Flow monitor commands
| 04-PTP commands | 154.58 KB |
display ptp foreign-masters-record
ptp alarm-threshold clock-source-class
ptp alarm-threshold time-offset
PTP commands
display ptp clock
Use display ptp clock to display PTP clock information.
display ptp clock
This command takes effect only after you specify a PTP profile (PTP standard) or a PTP clock node type.
# Display PTP clock information.
<Sysname> display ptp clock
PTP profile : IEEE 1588 Version 2
PTP mode : BC
Slave only : No
Clock ID : 000FE2-FFFE-FF0000
Clock type : ToD0
ToD direction : In
ToD delay time : 0 (ns)
Clock domain : 0
Number of PTP ports : 2
Priority1 : 128
Priority2 : 128
Clock quality :
Class : 6
Accuracy : 32
Offset (log variance) : 65535
Offset from master : 0 (ns)
Mean path delay : 0 (ns)
Steps removed : 0
Local clock time : Sun Jan 15 20:57:29 2011
PTP profile |
PTP standard. The value is IEEE 1588 version 2. |
PTP mode |
Clock node type: · BC. · E2ETC. · E2ETC-OC. · OC. · P2PTC. · P2PTC-OC. |
Slave only |
Whether the OC operates in Slave only mode: · Yes. · No. |
Clock ID |
Clock ID for the device, which uniquely identifies a PTP device. |
Clock type |
Clock type of the device: · Local—Local clock. · ToD0—ToD 0 clock. · ToD1—ToD 1 clock. |
ToD direction |
ToD input or output: · IN—The device receives clock signals from an external ToD clock. · Out—The device transmits ToD clock signals as a master. · N/A—The device neither receives nor transmits ToD clock signals. This field is not displayed for a local clock. |
ToD delay time |
Delay correction value in nanoseconds for the ToD clock. This field is not displayed when the device is a local clock. |
Clock domain |
PTP domain where the device resides. |
Priority1 |
Priority 1 value for the device. |
Priority2 |
Priority 2 value for the device. |
Class |
Time class of the device. |
Accuracy |
Time accuracy of the device. |
Offset (log variance) |
Offset of the grandmaster clock. |
Offset from master |
Offset from the master clock node (parent clock node), in nanoseconds. N/A indicates that information for this field is not obtained. |
Mean path delay |
Mean path delay, in nanoseconds. N/A indicates that information for this field is not obtained. |
Steps removed |
Hops from the grandmaster to the local clock node. N/A indicates that information for this field is not obtained. |
display ptp corrections
Use display ptp corrections to display PTP corrections that have occurred on a subordinate port.
The PTP corrections are displayed only when the following conditions are met:
· You have specified a PTP profile and PTP clock node type for the device.
· The device has a subordinate port and has performed time or frequency synchronization through the port.
If the subordinate port is changed, the recorded information will be cleared.
# Display PTP corrections that have occurred on a subordinate port.
<Sysname> display ptp corrections
Slave port Correction time Corrections(s,ns) Rate ratio
XGE3/1/1 Mar 11 03:14:54 2012 0,74 0.999999973
XGE3/1/1 Mar 11 03:14:55 2012 -1,17 0.999999980
Slave port |
Name of the subordinate port. |
Correction time |
Time when the correction occurred. |
Corrections(s,ns) |
Time corrections in seconds or nanoseconds. N/A indicates that no correction occurred this time. |
Rate ratio |
Ratio of the subordinate port rate to the master port rate. N/A indicates that no correction occurred this time. |
Use display ptp foreign-masters-record to display information about foreign master nodes.
display ptp foreign-masters-record [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays information about foreign master nodes for all interfaces.
Foreign master node information is displayed only when the following conditions are met:
· You have specified a PTP clock node type for the device.
· The device has a PTP port in slave or uncalibrated state.
# Display information about foreign master nodes for all interfaces.
<Sysname> display ptp foreign-masters-record
P1=Priority1, P2=Priority2, C=Class, A=Accuracy,
OSLV=Offset-scaled-log-variance, SR=Steps-removed
GM=Grandmaster
Interface Clock ID P1 P2 C A OSLV SR GM
XGE3/1/1 000FE2-FFFE-FF0000 0 128 248 37 65535 0 Yes
XGE3/1/2 000FE2-FFFE-FF0001 0 128 248 37 65535 1 No
Name of a PTP interface. |
Clock ID |
Clock ID of the foreign master node. |
C |
Time class. |
A |
Time accuracy. |
OSLV |
SR |
Hops from the grandmaster to the local clock node. |
GM |
Whether the node represents the grandmaster clock: · Yes. · No. |
display ptp interface
Use display ptp interface to display PTP running information for an interface.
display ptp interface [ interface-type interface-number | brief ]
interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays PTP running information for all interfaces.
brief: Displays brief PTP running information for all interfaces. If you do not specify this keyword, this command displays detailed PTP running information for the specified interface or all interfaces.
The detailed PTP running information can be displayed only if you enable PTP on the interface. The brief PTP running information can be displayed only when PTP is operating on the interface.
# Display brief PTP running information for all interfaces.
<Sysname> display ptp interface brief
Name State Delay mechanism Clock step Asymmetry correction
XGE3/1/1 Slave E2E Two 0
XGE3/1/2 Passive E2E Two 0
# Display detailed PTP running information for Ten-GigabitEthernet 3/1/1.
<Sysname> display ptp interface ten-gigabitethernet 3/1/1
Port number : 15
PTP version : 2
PTP enable : Enabled
Transport of PTP : User Datagram Protocol (IPv4)
Unicast destination address : 10.10.10.2
DSCP priority : 56
Port state : Slave
Force state : No
Clock step : Two
Asymmetry correction : 0
Delay mechanism : End to End
Announce interval (log mean) : 1
Announce receipt time out : 3
Sync interval (log mean) : 2
Delay request interval (log mean) : 2
Peer delay request interval (log mean) : 0
Name |
Name of the PTP interface. |
State |
States of the PTP interface: · Slave—Receives synchronization messages. · Uncalibrated—Temporary state before the interface enters Slave state. · Passive—Neither receives nor sends synchronization messages. A PTP interface is in passive state after it receives an announce messages. · Master—Sends synchronization messages. · Premaster—Temporary state before the interface enters Master state. · Listening—Neither receives nor sends synchronization messages. A PTP interface is in listening state after being initialized. · Faulty—PTP is running incorrectly. A PTP interface in faulty state does not process PTP messages. · Disabled—PTP is not running on the interface. A PTP interface in disabled state does not process PTP messages. · Initializing—The interface is initializing. A PTP interface in initializing state does not process PTP messages. · N/A—No PTP interface state is obtained. |
Delay mechanism |
Delay measurement mechanism: · End to End—Request-response mechanism. · Peer to Peer—Peer delay mechanism. |
Clock step |
Mode for carrying timestamps, fixed at Two, which represents the two-step mode. |
Asymmetry correction |
Asymmetric delay correction value (in nanoseconds). |
Clock ID |
Clock ID of the device where the interface resides. |
PTP version |
PTP version number. The version number is always 2. |
PTP enable |
Whether PTP is enabled or disabled: · Enabled. · Disabled. |
Transport of PTP |
PTP message transport protocol: · User Datagram Protocol (IPv4). · IEEE 802.3/Ethernet. |
Unicast destination address |
Destination IP address for unicast PTP messages that are transmitted over UDP. This field is not displayed if the ptp unicast-destination command is not executed. |
DSCP priority |
DSCP value for PTP messages that are transmitted over UDP. This field is not displayed if the ptp dscp command is not executed. |
VLAN |
VLAN ID for PTP messages. This field is not displayed if the ptp vlan command is not executed. |
Dot1p priority |
802.1p precedence for PTP messages. This field is not displayed if the ptp vlan command is not executed. |
Force state |
Whether the force state is configured: · Yes. · No. |
Announce interval (log mean) |
Announce message sending interval (in seconds) = 2internal. This field displays the value for the interval exponent. |
Announce receipt time out |
Number of announcement intervals before the receiving node stops receiving announce messages. If a member node does not receive any announce message from the master node within the specified value, it considers the master node invalid. |
Sync interval (log mean) |
Sync message sending interval (in seconds) = 2internal. This field displays the value for the interval exponent. |
Delay request interval (log mean) |
Minimum delay request message sending interval (in seconds) = 2internal. This field displays the value for the interval exponent. |
Peer delay request interval (log mean) |
Peer delay request message sending interval (in seconds) = 2internal. This field displays the value for the interval exponent. |
Mean path delay |
Mean path delay, in nanoseconds. |
display ptp parent
Use display ptp parent to display parent node (master node) information for the PTP device.
display ptp parent
The command does not display any information in any of the following circumstances:
· No PTP profile is specified.
· No PTP clock node type is specified, or the PTP clock node type is TC.
· The ptp active force-state command has been executed.
# Display parent node information for the PTP device.
<Sysname> display ptp parent
Parent clock:
Parent clock ID : 000FE2-FFFE-FF0005
Parent port number : 15
Observed parent offset (log variance) : N/A
Observed parent clock phase change rate : N/A
Grandmaster clock:
Grandmaster clock ID: 000FE2-FFFE-FF0000
Grandmaster clock quality:
Class : 248
Accuracy : 37
Priority1 : 128
Priority2 : 128
Table 5 Command output
Parent port number |
Outgoing interface number of the parent clock. |
Observed parent offset (log variance) |
Offset from the parent clock node. N/A indicates that information for this field is not obtained. |
Class |
Time class of the grandmaster clock. |
Accuracy |
Time accuracy of the grandmaster clock. |
Priority1 |
Priority 1 value of the grandmaster clock. |
Priority2 |
Priority 2 value of the grandmaster clock. |
display ptp path-trace
Use display ptp path-trace to display brief information about the PTP synchronization path from the GM to the device.
The command takes effect only after you specify a PTP profile or a PTP clock node type.
# Display brief information about the PTP synchronization path from the GM to the device.
<Sysname> display ptp path-trace
Sequence number Clock ID
2 000FE3-FFFE-F90000
3 000FE4-FFFE-F50000
4 000FE5-FFFE-F20000
5 000FE6-FFFE-F70000
Table 6 Command output
Sequence number |
Sequence number of the clock node |
Clock ID |
ID of the clock node |
display ptp statistics
Use display ptp statistics to display PTP statistics.
display ptp statistics [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command displays PTP statistics for all interfaces.
The command does not display any PTP statistics if you have not specified a PTP profile or a PTP clock node type.
# Display PTP statistics on Ten-GigabitEthernet 3/1/1.
<Sysname> display ptp statistics interface ten-gigabitethernet 3/1/1
Received packets
Announce :0 Sync :0 Signaling :0
DelayReq :0 DelayResp :0 FollowUp :0
PdelayReq:0 PdelayResp:0 PdelayRespFollowUp :0
Sent packets
Announce :476 Sync :2543 Signaling :0
DelayReq :0 DelayResp :0 FollowUp :2542
PdelayReq:238 PdelayResp:0 PdelayRespFollowUp :0
Discarded packets
Table 7 Command output
Received packets |
Statistics about received PTP messages. |
Sent packets |
Statistics about sent PTP messages. |
Discarded packets |
Statistics about discarded PTP messages. |
display ptp time-property
Use display ptp time-property to display PTP clock properties.
This command does not take effect in any of the following circumstances:
· You have not specified a PTP profile or a clock node type.
· You have specified the e2etc or p2ptc clock node type.
· You have executed the ptp active force-state command.
# Display PTP clock properties.
<Sysname> display ptp time-property
PTP clock time property:
Current UTC offset valid : True
Current UTC offset : 33
Leap59 : Yes
Leap61 : No
Time traceable : True
Frequency traceable : True
PTP timescale : True
Time source : 0xA0 (Internal oscillator)
Sync uncertain : False
Table 8 Command output
Current UTC offset valid |
Whether the UTC offset is valid: · True—Yes. · False—No. |
Current UTC offset |
Cumulative offset (in seconds) between the Coordinated Universal Time (UTC) of the grandmaster clock and the International Atomic Time (TAI). |
Leap59 |
Whether cumulative offset is minus 1: · Yes. · No. |
Leap61 |
Whether cumulative offset is plus 1: · Yes. · No. |
Time traceable |
Whether the PTP time is traceable: · True—Yes. · False—No. |
Frequency traceable |
Whether the PTP frequency is traceable: · True—Yes. · False—No. |
PTP timescale |
The possible timescales available for use by the grandmaster clock: · True—PTP timescale. · False—Non-PTP timescale. |
Time source |
Time source type of the grandmaster clock: · Atomic clock. · GPS. · Handset. · Internal oscillator. · NTP. · Other. · PTP. · Terrestrial radio. · Unknown. |
Sync uncertain |
Whether the upstream clock (master clock) is not reliable: · True—The upstream clock is not reliable. · False—The upstream clock is reliable. |
Use ptp active force-state to activate the port role configuration.
Use undo ptp active force-state to restore the default.
The port role configuration is not activated.
This command is available only after you specify a PTP profile and a PTP clock node type.
After you change the role of a PTP port, you must execute this command to activate the port role configuration.
# Activate the port role configuration.
[Sysname] ptp profile 1588v2
[Sysname] ptp mode oc
[Sysname] ptp active force-state
ptp force-state
ptp mode
ptp profile 1588v2
Use ptp alarm-threshold clock-source-class to set the class threshold for the clock source.
Use undo ptp alarm-threshold clock-source-class to restore the default.
ptp alarm-threshold clock-source-class class-value
The class threshold is 6 for the clock source.
class-value: Specifies a class threshold for the clock source, in the range of 0 to 255.
Each PTP clock source has a class value. For a ToD clock source, you can set its class value by using the ptp clock-source command. The higher the value, the lower the class. When the class value of the clock source crosses the threshold, the system outputs a log for notification.
This command is available only after you specify a PTP profile and PTP clock node type.
# Set the class threshold to 20 for the clock source.
[Sysname] ptp alarm-threshold clock-source-class 20
ptp clock-source
ptp mode
ptp profile 1588v2
Use ptp alarm-threshold time-offset to set the time-offset threshold between the external reference clock and the PTP clock.
Use undo ptp alarm-threshold time-offset to restore the default.
ptp alarm-threshold time-offset time-offset-value
The time-offset threshold between the external reference clock and the PTP clock is 500.
time-offset-value: Specifies the time-offset threshold between the external reference clock and the PTP clock, in the range of 200 to 1000, in nanoseconds.
If the device uses an external reference clock, it periodically calculates the time offset between the external reference clock and the PTP clock. When the offset exceeds the threshold, the device outputs a log for notification.
# Set the time-offset threshold between the external reference clock and the PTP clock to 800.
[Sysname] ptp alarm-threshold time-offset 800
ptp mode
ptp profile 1588v2
ptp announce-interval
Use ptp announce-interval to set the interval for sending announce messages.
Use undo ptp announce-interval to restore the default.
ptp announce-interval interval
The value of the interval argument is 1 and the announce message sending interval is 2 (21) seconds.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending announce messages. The value range for the interval argument is 0 to 4.
# Set the announce message sending interval to 4 (22) seconds on Ten-GigabitEthernet 3/1/1.
[Sysname] interface ten-gigabitethernet 3/1/1
[Sysname-Ten-GigabitEthernet3/1/1] ptp announce-interval 2
ptp mode
ptp profile 1588v2
ptp announce-timeout
Use ptp announce-timeout to set the timeout multiplier for the announce message receiving interval.
Use undo ptp announce-timeout to restore the default.
ptp announce-timeout multiple-value
The timeout multiplier for the announce message receiving interval is 3.
multiple-value: Sets the timeout multiplier for the announce message receiving interval, in the range of 2 to 10.
A master node periodically sends announce messages to the member nodes. If a member node does not receive any announce message from the master node within multiple-value times the announce message sending interval configured on the master node, it determines that the master node is invalid.
To ensure a stable PTP network, set the timeout multiplier for receiving announce messages to a value in the range of 5 to 7.
# Set the timeout multiplier for the announce message sending interval to 5 on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp announce-timeout 5
ptp mode
ptp profile 1588v2
ptp asymmetry-correction
Use ptp asymmetry-correction to set the asymmetric delay correction time.
Use undo ptp asymmetry-correction to restore the default.
ptp asymmetry-correction { minus | plus } value
The asymmetric delay correction time is 0 nanoseconds, which means that delay correction is not performed.
minus: Subtracts the specified asymmetric delay correction value.
plus: Adds the specified asymmetric delay correction value.
value: Specifies the asymmetric delay correction value in the range of 0 to 2000000 nanoseconds.
# Set the asymmetric delay correction time to 100 nanoseconds on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp asymmetry-correction plus 100
ptp mode
ptp profile 1588v2
ptp clock-source
Use ptp clock-source to configure ToD clock parameters.
Use undo ptp clock-source to restore ToD clock parameters to their default values.
ptp clock-source { tod0 | tod1 } { accuracy acc-value | class class-value | time-source ts-value }
undo ptp clock-source { tod0 | tod1 } { accuracy | class | time-source }
For a ToD clock, the accuracy is 32, the clock class is 6, and the attribute value is 32.
tod0: Specifies the ToD 0 clock. This keyword is not supported in the current software version.
tod1: Specifies the ToD 1 clock.
accuracy acc-value: Specifies the accuracy of the ToD clock, in the range of 0 to 255. A smaller value indicates a higher accuracy. Table 9 shows the description for clock accuracy values.
Table 9 Clock accuracy value description
Clock accuracy value (in hexadecimal format) |
00 through 1F |
Reserved. |
20 |
Less than 25 nanoseconds (1 nanosecond = 10-9 second). |
21 |
Less than 100 nanoseconds. |
22 |
Less than 250 nanoseconds. |
23 |
Less than 1 microsecond (10-6 second). |
24 |
Less than 2.5 microseconds. |
25 |
Less than 10 microseconds. |
26 |
Less than 25 microseconds. |
27 |
Less than 100 microseconds. |
28 |
Less than 250 microseconds. |
29 |
Less than 1 millisecond (10-3 second). |
2A |
Less than 2.5 milliseconds. |
2B |
Less than 10 milliseconds. |
2C |
Less than 25 milliseconds. |
2D |
Less than 100 milliseconds. |
2E |
Less than 250 milliseconds. |
2F |
Less than 1 second. |
30 |
Less than 10 seconds. |
31 |
More than 10 seconds. |
32 through 7F |
Reserved. |
80 through FD |
For use by alternate PTP profiles. |
FE |
Unknown. |
FF |
Reserved. |
class class-value: Specifies the class of the ToD clock, in the range of 0 to 255. A smaller value indicates a higher time class. Table 10 shows the description for clock classes. The values not listed in the table are reserved by the protocol. As a best practice, do not use those values.
Table 10 Clock class description
Clock class (in decimal format) |
6 |
The clock node synchronizes its time to the master reference time source. PTP assigns a time table to the clock node. A clock node with time class 6 cannot become a member clock of any other clocks in the domain. |
7 |
The former time class is 6. The clock node cannot synchronize its time to a time source. It enters the reappointment mode and meets the reappointment conditions. PTP assigns a time table to the clock node. A clock node with time class 7 cannot become a member clock of any other clocks in the domain. |
13 |
The clock node synchronizes its time to a time source. ARB assigns a time table to the clock node. A clock node with time class 13 cannot become a member clock of any other clocks in the domain. |
14 |
The former time class is 13. The clock node cannot synchronize its time to a time source. It enters the reappointment mode and meets the reappointment conditions. ARB assigns a time table to the clock node. A clock node with time class 14 cannot become a member clock of any other clocks in the domain. |
52 |
The clock node with time class 7 becomes optional clock A because it does not meet the reappointment conditions. A clock node with time class 52 cannot become a member clock of any other clocks in the domain. |
58 |
The clock node with time class 14 becomes optional clock A because it does not meet the reappointment conditions. A clock node with time class 58 cannot become a member clock of any other clocks in the domain. |
187 |
The clock node with time class 7 becomes optional clock B because it does not meet the reappointment conditions. A clock node with time class 187 can become a member clock of another clock in the domain. |
193 |
The clock node with time class 14 becomes optional clock B because it does not meet the reappointment conditions. A clock node with time class 193 can become a member clock of another clock in the domain. |
248 |
Default time class value. |
255 |
Clock node operating in slave-only mode. |
time-source ts-value: Specifies the clock attribute value in the range of 0 to 255. Table 11 shows the description for the clock attribute values (those not listed are reserved for the protocol).
Table 11 GM attribute value description
GM attribute values (in hexadecimal format) |
10 |
Atomic clock. |
20 |
GPS. |
30 |
Terrestrial radio. |
40 |
PTP. |
50 |
NTP. |
60 |
Handset. |
90 |
Other. |
A0 |
Internal oscillator. |
F0 to FE |
FF |
Reserved. |
# Configure the time accuracy for the ToD 0 clock as 44.
[Sysname] ptp clock-source tod0 accuracy 44
ptp mode
ptp profile 1588v2
ptp clock-step
Use ptp clock-step to configure the mode for carrying timestamps.
Use undo ptp clock-step to restore the default.
ptp clock-step { one-step | two-step }
undo ptp clock-step
Two-step mode is used for carrying timestamps.
one-step: Specifies the single-step mode. This keyword is not supported in the current software version.
two-step: Specifies the two-step mode.
# Specify the two-step timestamp carrying mode on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp clock-step two-step
ptp mode
ptp profile 1588v2
ptp delay-mechanism
Use ptp delay-mechanism to specify a PTP delay measurement mechanism.
Use undo ptp delay-mechanism to restore the default.
ptp delay-mechanism { e2e | p2p }
The request-response delay measurement mechanism applies.
e2e: Specifies the request-response mechanism.
p2p: Specifies the peer delay mechanism.
You can configure this command only for BCs and OCs. The delay measurement mechanism is Request_Response for E2ETCs and E2ETC+OCs and Peer Delay for P2PTCs and P2PTC+OCs. You cannot change the delay measurement mechanism for these clock nodes.
# Specify the OC clock type. On Ten-GigabitEthernet 3/1/1, specify the request-response delay measurement mechanism (e2e).
[Sysname-Ten-GigabitEthernet3/1/1] ptp delay-mechanism e2e
ptp mode
ptp profile 1588v2
ptp destination-mac
Use ptp destination-mac to configure the destination MAC address for PTP messages.
Use undo ptp destination-mac to restore the default.
ptp destination-mac mac-address
The destination MAC address for non-peer delay messages is 011B-1900-0000.
The destination MAC address for peer delay messages is 0180-C200-000E.
mac-address: Specifies the destination MAC address (any unicast MAC address) for PTP unicast messages or specifies the destination MAC address (0180-C200-000E or 011B-1900-0000) for non-peer delay multicast messages.
This command is available only after you specify a PTP profile and specify a PTP clock node type.
This command takes effect only when PTP messages are encapsulated in IEEE 802.3/Ethernet packets.
IEEE 802.3/Ethernet-encapsulated PTP messages can be sent through multicast (default) or unicast.
· In multicast mode, the destination MAC address is 0180-C200-000E or 011B-1900-0000 for non-Pdelay messages and 0180-C200-000E for Pdelay messages. Non-Pdelay messages include delay_Req, delay_Resp, delay_Resp_Follow_Up, Announce, Sync, and FollowUp messages. Pdelay messages include Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages.
· In unicast mode, you can configure any unicast MAC address as the destination address for PTP messages.
# Configure 0180-C200-000E as the destination MAC address for non-peer delay messages on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp destination-mac 0180-c200-000e
ptp mode
ptp profile 1588v2
ptp domain
Use ptp domain to specify the PTP domain.
Use undo ptp domain to restore the default.
ptp domain domain-number
undo ptp domain
The device is in PTP domain 0.
domain-number: Specifies a PTP domain by its domain number in the range of 0 to 255.
# Specify PTP domain 2 for the device.
[Sysname] ptp domain 2
ptp mode
ptp profile 1588v2
ptp dscp
Use ptp dscp to set the DSCP value for UDP-encapsulated PTP messages.
Use undo ptp dscp to restore the default.
ptp dscp dscp
undo ptp dscp
The DSCP value is 56 for UDP-encapsulated PTP messages.
dscp: Sets a DSCP value in the range of 0 to 63.
This command takes effect only for UDP-encapsulated PTP messages.
# Set the DSCP value to 63 for UDP-encapsulated PTP messages on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp transport-protocol udp
[Sysname-Ten-GigabitEthernet3/1/1] ptp dscp 63
ptp mode
ptp profile 1588v2
ptp enable
Use ptp enable to enable PTP.
Use undo ptp enable to disable PTP.
ptp enable
undo ptp enable
PTP is disabled.
For an OC clock node, you can enable PTP only on one port.
As a best practice, enable PTP on an interface after you configure PTP parameters.
# Specify the OC clock node type, and enable PTP on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp enable
# Specify the E2ETC clock node type, and enable PTP on Ten-GigabitEthernet 3/1/1 and Ten-GigabitEthernet 3/1/2.
[Sysname] ptp mode e2etc
[Sysname-Ten-GigabitEthernet3/1/1] interface ten-gigabitethernet 3/1/2
[Sysname-Ten-GigabitEthernet3/1/2] ptp enable
ptp mode
ptp profile 1588v2
ptp force-state
Use ptp force-state to configure a role for a PTP port.
Use undo ptp force-state to restore the default.
ptp force-state { master | passive | slave }
The PTP port role is automatically calculated by BMC.
master: Specifies the PTP port as a master port.
passive: Specifies the PTP port as a passive port.
slave: Specifies the PTP port as a subordinate port.
You can configure only one subordinate port for a device.
After you change the role of a PTP port, you must execute the ptp active force-state command to activate the port role configuration.
# Specify the OC clock node type. Specify the PTP port Ten-GigabitEthernet 3/1/1 as a subordinate port.
[Sysname-Ten-GigabitEthernet3/1/1] ptp force-state slave
ptp mode
ptp profile 1588v2
ptp slave-only
ptp max-steps-removed
Use ptp max-steps-removed to specify the maximum number of removed steps (clock nodes) from the GM to the device.
Use undo ptp max-steps-removed to restore the default.
ptp max-steps-removed step-removed-value
The maximum number of removed steps is 255 from the GM to the device.
step-removed-value: Specifies the maximum number of removed steps from the GM to the device, in the range of 1 to 255.
If the number of removed steps from the GM to the device exceeds the maximum number, the device cannot synchronize time to the GM.
# Set the maximum number of removed steps from the GM to the device to 20.
[Sysname] ptp max-steps-removed 20
ptp mode
ptp profile 1588v2
ptp min-delayreq-interval
Use ptp min-delayreq-interval to set the minimum interval for sending delay request messages.
Use undo ptp min-delayreq-interval to restore the default.
ptp min-delayreq-interval interval
The minimum interval for sending delay request messages is 1 (20) second.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending delay request messages. The value range for the interval argument is –4 to 6.
When a member clock receives a Sync message, it responds by sending a Delay_Req message and starts a timer defined by this command. The member clock will not send another Delay_Req message until it receives a Sync message after the timer expires.
The configured interval takes effect only when it is set on the master clock. The master clock sends the value to a member clock through PTP messages to control the interval for the member clock to send Delay_Req messages. To view the value on a member clock, execute the display ptp interface command on the member clock.
# Set the minimum interval to 4 (22) seconds for sending delay request messages on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp min-delayreq-interval 2
ptp mode
ptp profile 1588v2
ptp syn-interval
ptp mode
Use ptp mode to specify a clock node type for the device.
Use undo ptp mode to restore the default.
ptp mode { bc | e2etc | e2etc-oc | oc | p2ptc | p2ptc-oc }
undo ptp mode
No clock node type is specified.
bc: Specifies the boundary clock (BC) type.
e2etc: Specifies the end-to-end transparent clock (E2ETC) type.
e2etc-oc: Specifies the E2ETC+OC type.
oc: Specifies the ordinary clock (OC) type.
p2ptc: Specifies the peer-to-peer transparent clock (P2PTC) type.
p2ptc-oc: Specifies the P2PTC+OC type.
CAUTION: If you change the clock node type for the device, all settings except for the PTP profile will be removed. |
The following restrictions apply for using this command:
· This command is available only after you specify a PTP profile.
· You can specify only one clock node type for a device.
· Changing or removing the clock node type will restore the default settings of the PTP profile.
# Specify the OC clock node type for the device.
ptp profile 1588v2
ptp pdelay-req-interval
Use ptp pdelay-req-interval to set the interval for sending peer delay request messages.
Use undo ptp pdelay-req-interval to restore the default.
ptp pdelay-req-interval interval
The interval for sending peer delay request messages is 1 (20) second.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending peer delay request messages. The value range for the interval argument is 0 to 5.
# Set the interval to 4 (22) seconds for sending peer delay request messages on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp pdelay-req-interval 2
ptp mode
ptp profile 1588v2
ptp port-mode
Use ptp port-mode to configure the port type as OC for a TC+OC (including E2ETC+OC and P2PTC+OC) clock.
Use undo ptp port-mode to restore the default.
ptp port-mode oc
undo ptp port-mode
The type of all ports on an E2ETC+OC or a P2PTC+OC clock is TC.
oc: Specifies the port type for a TC+OC clock as OC.
This command is available only after you specify a PTP profile and a PTP clock node type. Only E2ETC+OC and P2PTC+OC clock nodes support this command.
# Specify the P2PTC+OC clock node type for the device. Configure the port type for Ten-GigabitEthernet 3/1/1 as OC.
[Sysname] ptp mode p2ptc-oc
[Sysname-Ten-GigabitEthernet3/1/1] ptp port-mode oc
ptp mode
ptp profile 1588v2
ptp priority clock-source
Use ptp priority clock-source to configure the priority for the specified clock for GM election through BMC.
Use undo ptp priority clock-source to restore the specified priority to its default value.
ptp priority clock-source { local | tod0 | tod1 } { priority1 priority1| priority2 priority2 }
undo ptp priority clock-source { local | tod0 | tod1 } { priority1 | priority2 }
The priority 1 and priority 2 values are both 128.
local: Specifies the local clock.
priority1 priority1: Specifies priority 1 for the clock. The value is in the range of 0 to 255. A numerically smaller value has higher priority.
priority2 priority2: Specifies priority 2 for the clock. A numerically smaller value has higher priority. The value range for the argument is 0 to 255.
The local priority of a clock will not be carried in PTP announce messages.
# Set priority 1 to 10 for the local clock.
[Sysname] ptp priority clock-source local priority1 10
ptp mode
ptp profile 1588v2
ptp profile 1588v2
Use ptp profile 1588v2 to specify the IEEE 1588 version 2 PTP profile.
Use undo ptp profile to restore the default.
ptp profile 1588v2
undo ptp profile
No PTP profile is configured, and PTP is not running on the device.
You must first specify a PTP profile before configuring PTP commands.
Changing or removing a PTP profile clears all settings under the PTP profile.
# Specify the IEEE 1588 version 2 PTP profile.
ptp slave-only
Use ptp slave-only to configure the OC to operate only as a member clock.
Use undo ptp slave-only to restore the default.
ptp slave-only
undo ptp slave-only
An OC can operate either as a master clock or a member clock.
This command is applicable only to OCs and is available only after you specify a PTP profile and a PTP clock node type.
You can execute the ptp force-state command to specify a subordinate port as a master port or passive port even if the OC operates as a member clock.
# Specify the clock node type as OC for the device. Configure the OC to operate only as a member clock.
[Sysname] ptp slave-only
ptp force-state
ptp mode
ptp profile 1588v2
ptp source
Use ptp source to configure the source IP address for UDP-encapsulated multicast PTP messages.
Use undo ptp source to remove the specified source IP address for UDP-encapsulated multicast PTP messages.
ptp source ip-address [ vpn-instance vpn-instance-name ]
undo ptp source ip-address [ vpn-instance vpn-instance-name ]
No source IP address is configured for UDP-encapsulated multicast PTP messages.
ip-address: Specifies the source IP address for UDP-encapsulated multicast PTP messages.
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance used for communication between the local device and the peer device. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If the peer device belongs to the public network, do not specify this option.
This command is available only after you specify a PTP profile and a PTP clock type.
This command takes effect only for UDP-encapsulated multicast PTP messages.
# Specify 3.5.1.5 as the source address for UDP-encapsulated multicast PTP messages.
[Sysname] ptp source 3.5.1.5
ptp mode
ptp profile 1588v2
ptp syn-interval
Use ptp syn-interval to set the interval for sending Sync messages.
Use undo ptp syn-interval to restore the default.
ptp syn-interval interval
The value of the interval argument is 0 and the interval for sending Sync messages is 1 (20) second.
interval: Specifies an exponent, to the power of which base 2 is raised to get the interval in seconds for sending Sync messages. The value range for the interval argument is–1 to 1.
# Set the Sync message sending interval to 2 (21) seconds on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp syn-interval 1
ptp mode
ptp profile 1588v2
ptp { tod0 | tod1 }
Use ptp { tod0 | tod1 } to configure ToD input or output.
Use undo ptp { tod0 | tod1 } to restore the default delay correction value.
ptp tod0 input [ delay input-delay-time ]
undo ptp tod0 input
ptp tod1 output [ delay output-delay-time ]
undo ptp tod1 output
Whether to transmit or receive ToD signals is not configured.
input: Specifies the input direction for the device to receive ToD clock signals. It can be used only with the tod0 keyword, not the tod1 keyword.
input-delay-time: Specifies the delay correction value for receiving ToD clock signals. The value range for this argument is 0 to 2000000, in nanoseconds. The default value is 0.
output: Specifies the output direction for the device to send ToD clock signals as a master. It can be used only with the tod1 keyword, not the tod0 keyword.
output-delay-time: Specifies the delay correction value for sending ToD clock signals. The value range for this argument is 0 to 1600, in nanoseconds. The default value is 0.
For the undo form of the command to take effect, first modify ToD input or output settings by executing this command.
# Set the delay correction value to 1000 nanoseconds for receiving ToD 0 clock signals.
[Sysname] ptp tod0 input delay 1000
ptp mode
ptp profile 1588v2
Use ptp transport-protocol to specify UDP encapsulation for PTP messages.
Use undo ptp transport-protocol to restore the default.
PTP messages are IEEE 802.3/Ethernet-encapsulated.
udp: Specifies UDP encapsulation.
# Specify UDP encapsulation for PTP messages on Ten-GigabitEthernet 3/1/1.
ptp mode
ptp profile 1588v2
Use ptp unicast-destination to configure the unicast destination IP address for UDP-encapsulated PTP messages.
Use undo ptp unicast-destination to restore the default.
ptp unicast-destination ip-address
undo ptp unicast-destination ip-address
No unicast destination IP address is configured for UDP-encapsulated PTP messages.
ip-address: Specifies the unicast destination IP address for UDP-encapsulated PTP messages.
# Configure 10.10.10.2 as the unicast destination address for UDP-encapsulated PTP messages.
[Sysname-Ten-GigabitEthernet3/1/1] ptp unicast-destination 10.10.10.2
ptp mode
ptp profile 1588v2
ptp utc
Use ptp utc to set the correction date for the UTC.
Use undo ptp utc to remove the correction date configured for the UTC.
ptp utc { leap59-date | leap61-date } date
undo ptp utc { leap59-date | leap61-date }
No correction date is configured for the UTC.
leap59-date: Adjusts the UTC at the last minute (23:59) of the specified date so that the UTC is one second slower than the TAI.
leap61-date: Adjusts the UTC at the last minute (23:59) of the specified date so that the UTC is one second faster than the TAI.
date: Sets the date to adjust the UTC, in the format of YYYY/MM/DD. The value range for YYYY and MM is 2000 to 2035 and 1 to 12, respectively. The value range for DD depends on the specified month. For the configuration to take effect, do not specify a date earlier than the current date.
Specify either the leap59-date or leap61-date keyword in this command. If you execute this command multiple times, the most recent configuration takes effect.
# Assume the current date is August 8, 2010. Specify the clock node type as BC for the device. Adjust the UTC at the last minute of December 31, 2010 so that the UTC is one second slower than the TAI.
[Sysname] ptp mode bc
[Sysname] ptp utc leap59-date 2010/12/31
ptp mode
ptp profile 1588v2
ptp utc offset
Use ptp utc offset to set the cumulative offset between the UTC and TAI.
Use undo ptp utc offset to restore the default.
ptp utc offset utc-offset
undo ptp utc offset
The cumulative offset between the UTC and TAI is 0 seconds.
utc-offset: Sets the cumulative offset between the UTC and TAI. The value range for this argument is 0 to 999, in seconds.
# Set the cumulative offset to 33 seconds between the UTC and TAI.
[Sysname] ptp utc offset 33
ptp mode
ptp profile 1588v2
ptp vlan
Use ptp vlan to specify a VLAN tag for PTP messages.
Use undo ptp vlan to restore the default.
ptp vlan vlan-id [ dot1p dot1p-value ]
undo ptp vlan [ dot1p ]
PTP messages do not have a VLAN tag.
vlan vlan-id: Specifies a VLAN by its ID in the range of 1 to 4094.
dot1p dot1p-value: Specifies an 802.1p precedence for PTP messages. The value range is 0 to 7. The default is 7. The device uses the default value 7 regardless of your setting.
# Specify VLAN 2 and set the 802.1p precedence to 6 for PTP messages on Ten-GigabitEthernet 3/1/1.
[Sysname-Ten-GigabitEthernet3/1/1] ptp vlan 2 dot1p 6
ptp mode
ptp profile 1588v2
reset ptp statistics
Use reset ptp statistics to clear PTP statistics.
reset ptp statistics [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies an interface by its type and number. If you do not specify an interface, this command clears PTP statistics on all interfaces.
# Clear PTP statistics on Ten-GigabitEthernet 3/1/1.
<Sysname> reset ptp statistics interface ten-gigabitethernet 3/1/1
