12-Network Management and Monitoring Command Reference
HomeSupportSwitchesS10500 SeriesReference GuidesCommand ReferencesH3C S10500 Command References-R7523P01-6W10012-Network Management and Monitoring Command Reference
03-NTP commands
03-NTP commands 182.44 KB
NTP commands
NTP is supported on the following Layer 3 interfaces:
·     Layer 3 Ethernet interfaces.
·     Layer 3 Ethernet subinterfaces.
·     Layer 3 aggregate interfaces.
·     Layer 3 aggregate subinterfaces.
·     VLAN interfaces.
·     Tunnel interfaces.
display ntp-service ipv6 sessions
Use display ntp-service ipv6 sessions to display information about all IPv6 NTP associations.
display ntp-service ipv6 sessions [ verbose ]
verbose: Displays detailed information about all IPv6 NTP associations. If you do not specify this keyword, the command displays only brief information about the IPv6 NTP associations.
# Display brief information about all IPv6 NTP associations.
<Sysname> display ntp-service ipv6 sessions
 Source:   [125]3000::32
 Reference: 127.127.1.0           Clock stratum: 2
 Reachabilities: 1                Poll interval: 64
 Last receive time: 6             Offset: -0.0
 Roundtrip delay: 0.0             Dispersion: 0.0
 Total sessions : 1
[12345]
·     1—Clock source selected by the system (the current reference source).
·     2—The stratum level of the clock source is less than or equal to 15.
·     3—The clock source has survived the clock selection algorithm.
·     4—The clock source is a candidate clock source.
·     5—The clock source was created by a command.
Source
IPv6 address of the NTP server. If this field displays ::, the IPv6 address of the NTP server has not been resolved successfully.
Reference
Reference clock ID of the NTP server:
·     If the reference clock is the local clock, the value of this field is related to the value of the Clock stratum field:
¡     When the value of the Clock stratum field is 0 or 1, this field displays LOCL.
¡     When the Clock stratum field has another value, this field displays the MD5 digest value of the first 32 bits of the IPv6 address. The MD5 digest value is in dotted decimal format.
·     If the reference clock is the clock of another device on the network, this field displays the MD5 digest value of the first 32 bits of the IPv6 address. The MD5 digest value is in dotted decimal format. If this field displays INIT, the local device has not established a connection with the NTP server.
Clock stratum
Stratum level of the NTP server, which determines the clock accuracy. The value is in the range of 1 to 16. A lower stratum level represents higher clock accuracy. A stratum 16 clock is not synchronized and cannot be used as a reference clock.
Reachabilities
Reachability count of the NTP server. 0 indicates that the NTP server is unreachable.
Poll interval
Polling interval in seconds. It is the maximum interval between successive NTP messages.
Last receive time
Length of time from when the last NTP message was received or when the local clock was last updated to the current time.
Time is in seconds by default.
·     If the time length is greater than 2048 seconds, it is displayed in minutes (m).
·     If the time length is greater than 300 minutes, it is displayed in hours (h).
·     If the time length is greater than 96 hours, it is displayed in days (d).
·     If the time length is greater than 999 days, it is displayed in years (y).
If the time when the most recent NTP message was received or when the local clock was updated most recently is behind the current time, this field displays a hyphen (-).
Offset
Offset of the system clock relative to the reference clock, in milliseconds.
Roundtrip delay
Roundtrip delay from the local device to the clock source, in milliseconds.
Dispersion
Maximum error of the system clock relative to the reference source.
Total sessions
Total number of associations.
# Display detailed information about all IPv6 NTP associations.
<Sysname> display ntp-service ipv6 sessions verbose
 Clock source: 1::1
 Session ID: 36144
 Clock stratum: 16
 Clock status:  configured, insane, valid, unsynced
 Reference clock ID: INIT
 VPN instance: Not specified
 Local mode: sym_active, local poll interval: 6
 Peer mode: unspec, peer poll interval: 10
 Offset: 0.0000ms, roundtrip delay: 0.0000ms, dispersion:  15937ms
 Root roundtrip delay: 0.0000ms, root dispersion: 0.0000ms
 Reachabilities:0, sync distance: 15.938
 Precision: 2^10, version: 4, source interface: Not specified
 Reftime: 00000000.00000000  Thu, Feb  7 2036  6:28:16.000
 Orgtime: d17cbb21.0f318106  Tue, May 17 2011  9:15:13.059
 Rcvtime: 00000000.00000000  Thu, Feb  7 2036  6:28:16.000
 Xmttime: 00000000.00000000  Thu, Feb  7 2036  6:28:16.000
 Roundtrip delay samples: 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
 Offset samples: 0.00  0.00  0.00  0.00  0.00  0.00  0.00  0.00
 Filter order: 0     1     2     3     4     5     6     7
 Total sessions: 1
Clock source
IPv6 address of the clock source. If this field displays ::, the IPv6 address of the NTP server has not been resolved successfully.
Clock stratum
Stratum level of the NTP server, which determines the clock precision. The value is in the range of 1 to 16. A lower stratum level represents higher clock accuracy. A stratum 16 clock is not synchronized and cannot be used as a reference clock.
Clock status
Status of the clock source corresponding to this association:
·     configured—The association was created at the CLI.
·     dynamic—The association is established dynamically.
·     master—The clock source is the primary reference source of the current system.
·     selected—The clock source has survived the clock selection algorithm.
·     candidate—The clock source is the candidate reference source.
·     sane—The clock source has passed authentication and will be used as a reference clock.
·     insane—The clock source has not passed authentication, or it has passed authentication but will not be used as a reference clock.
·     valid—The clock source is valid, which means the clock source meets the following requirements:
¡     It has been authenticated and synchronized.
¡     Its stratum level is valid.
¡     Its root delay and root dispersion values are within their ranges.
·     invalid—The clock source is invalid.
·     unsynced—The clock source has not been synchronized or the value of the stratum level is invalid.
Reference clock ID
VPN instance
VPN instance of the NTP server. If the NTP server is in a public network, this field displays Not specified.
Local mode
Operation mode of the local device:
·     unspec—The mode is unspecified.
·     sym_active—Active mode.
·     sym_passive—Passive mode.
·     client—Client mode.
·     server—Server mode.
·     broadcast—Broadcast or multicast server mode.
·     bclient—Broadcast or multicast client mode.
local poll interval
Polling interval for the local device, in seconds. The value displayed is a power of 2. For example, if the displayed value is 6, the poll interval of the local device is 26, or 64 seconds.
peer mode
Operation mode of the peer device:
peer poll interval
Polling interval for the peer device, in seconds. The value displayed is a power of 2. For example, if the displayed value is 6, the polling interval of the local device is 26, or 64 seconds.
Offset
roundtrip delay
dispersion
Maximum error of the system clock relative to the reference clock.
Roundtrip delay from the local device to the primary reference source, in milliseconds.
root dispersion
Maximum error of the system clock relative to the primary reference clock, in milliseconds.
Reachabilities
Reachability count of the clock source. 0 indicates that the clock source is unreachable.
sync distance
Synchronization distance relative to the upper-level clock, in seconds, and calculated from dispersion and roundtrip delay values.
Precision
Accuracy of the system clock.
version
NTP version in the range of 1 to 4.
source interface
Source interface.
If the source interface is not specified, this field displays Not specified.
Reftime
Reference timestamp in the NTP message.
Orgtime
Originate timestamp in the NTP message.
Rcvtime
Receive timestamp in the NTP message.
Xmttime
Transmit timestamp in the NTP message.
Filter order
Dispersion information.
Reference clock status
Status of the local clock. The field is displayed only when you use the ntp-service refclock-master command to set the local clock as a reference clock.
When the reach field of the local clock is 255, the field is displayed as working normally. Otherwise, the field is displayed as working abnormally.
Total sessions
display ntp-service sessions
Use display ntp-service sessions to display information about all IPv4 NTP associations.
display ntp-service sessions [ verbose ]
verbose: Displays detailed information about all IPv4 NTP associations. If you do not specify this keyword, the command displays only brief information about the NTP associations.
When a device is operating in NTP broadcast or multicast server mode, the display ntp-service sessions command does not display the IPv4 NTP association information corresponding to the broadcast or multicast server. However, the associations are counted in the total number of associations.
# Display brief information about all IPv4 NTP associations.
<Sysname> display ntp-service sessions
       source          reference       stra reach poll  now offset  delay disper
[12345]LOCAL(0)        LOCL               0     1   64    - 0.0000 0.0000 7937.9
    [5]0.0.0.0         INIT              16     0   64    - 0.0000 0.0000 0.0000
 Total sessions: 1
source
·     When the reference clock is the local clock, the field displays LOCAL (number). It indicates that the IP address of the local clock is 127.127.1.number, where number represents the NTP process number in the range of 0 to 3.
·     When the reference clock is the clock of another device, the field displays the IP address of the NTP server. If this field displays 0.0.0.0, the IP address of the NTP server has not been resolved successfully.
reference
·     If the reference clock is the local clock, the value of this field is related to the value of the stra field:
¡     When the value of the stra field is 0 or 1, this field displays LOCL.
¡     When the stra field has another value, this field displays the IP address of the local clock.
·     If the reference clock is the clock of another device on the network, this field displays the IP address of the device. If the device supports IPv6, this field displays the MD5 digest of the first 32 bits of the IPv6 address of the device. If this field displays INIT, the local device has not established a connection with the NTP server.
stra
Stratum level of the clock source, which determines the clock accuracy. The value is in the range of 1 to 16. The clock accuracy decreases from stratum 1 to stratum 16. A stratum 1 clock has the highest precision, and a stratum 16 clock is not synchronized and cannot be used as a reference clock.
reach
poll
now
offset
delay
Roundtrip delay from the local device to the NTP server, in milliseconds.
disper
Maximum error of the system clock relative to the reference source, in milliseconds.
[12345]
·     5—The clock source was created by a configuration command.
Total sessions
# Display detailed information about all IPv4 NTP associations.
<Sysname> display ntp-service sessions verbose
 Clock source: 192.168.1.40
 Session ID: 35888
 Clock stratum: 2
 Clock status:  configured, master, sane, valid
 Reference clock ID: 127.127.1.0
 Local mode: client, local poll interval: 6
 Peer mode: server, peer poll interval: 6
 Offset: 0.2862ms, roundtrip delay: 3.2653ms, dispersion: 4.5166ms
 Root roundtrip delay: 0.0000ms, root dispersion: 10.910ms
 Reachabilities:31, sync distance: 0.0194
 Precision: 2^18, version: 3, source interface: Not specified
 Reftime: d17cbba5.1473de1e  Tue, May 17 2011  9:17:25.079
 Orgtime: 00000000.00000000  Thu, Feb  7 2036  6:28:16.000
 Rcvtime: d17cbbc0.b1959a30  Tue, May 17 2011  9:17:52.693
 Xmttime: d17cbbc0.b1959a30  Tue, May 17 2011  9:17:52.693
 Roundtrip delay samples: 0.007 0.010 0.006 0.011 0.010 0.005 0.007 0.003
 Offset samples: 5629.55 3913.76 5247.27 6526.92 31.99 148.72 38.27 0.29
 Filter order: 7     5     2     6     0     4     1     3
 Total sessions: 1
Clock source
Clock stratum
Stratum level of the NTP server, which determines the clock accuracy. The value is in the range of 1 to 16. A lower stratum level represents greater clock accuracy. A stratum 16 clock is not synchronized and cannot be used as a reference clock.
Clock status
·     configured—The association was created by a configuration command.
Reference clock ID
¡     When the Clock stratum field has another value, this field displays the IP address of the local clock.
VPN instance
VPN instance to which the NTP server belongs. If the NTP server is in a public network, the field displays Not specified.
Local mode
·     active—Active mode.
·     passive—Passive mode.
local poll interval
Polling interval of the local device, in seconds. The value displayed is a power of 2. For example, if the displayed value is 6, the poll interval of the local device is 26, or 64 seconds.
Peer mode
peer poll interval
Polling interval of the peer device, in seconds. The value displayed is a power of 2. For example, if the displayed value is 6, the poll interval of the local device is 26, or 64 seconds.
Offset
roundtrip delay
dispersion
root dispersion
Reachabilities
sync distance
Precision
version
source interface
Source interface.
If the source interface is not specified, this field is Not specified.
Reftime
Orgtime
Rcvtime
Xmttime
Filter order
Sample information order.
Total sessions
display ntp-service status
Use display ntp-service status to display NTP service status.
# Display NTP service status after time synchronization.
<Sysname> display ntp-service status
 Clock status: synchronized
 Clock stratum: 2
 System peer: LOCAL(0)
 Local mode: client
 Leap indicator: 00
 Clock jitter: 0.000977 s
 Stability: 0.000 pps
 Clock precision: 2^-18
Root delay: 0.00000 ms
 Root dispersion: 3.96367 ms
 Reference time: d0c5fc32.92c70b1e  Wed, Dec 29 2010 18:28:02.573
# Display the NTP service status when time is not synchronized.
 Clock status: unsynchronized
 Clock stratum: 16
 Reference clock ID: none
 Clock jitter: 0.000000 s
 Root dispersion: 0.00002 ms
Table 5 Command output
Clock status
Status of the system clock:
·     synchronized—The system clock has been synchronized.
·     unsynchronized—The system clock has not been synchronized.
Clock stratum
Stratum level of the system clock.
System peer
IP address of the selected NTP server.
Local mode
Reference clock ID
For an IPv4 NTP server:
The field represents the IP address of the remote server when the local device is synchronized to a remote NTP server.
The field represents the local clock when the local device uses the local clock as a reference source.
·     When the local clock has a stratum level of 1, this field displays LOCL.
·     When the local clock has any other stratum, this field displays the IP address of the local clock.
For an IPv6 NTP server:
The field represents the MD5 digest of the first 32 bits of the IPv6 address of the remote server when the local device is synchronized to a remote IPv6 NTP server.
·     When the local clock has any other stratum, this field displays the MD5 digest of the first 32 bits of the IPv6 address of the local clock.
Leap indicator
Alarming status:
·     00—Normal.
·     01—Leap second, indicates that the last minute in a day has 61 seconds.
·     10—Leap second, indicates that the last minute in a day has 59 seconds.
·     11—Time is not synchronized.
Clock jitter
Difference between the system clock and reference clock, in seconds.
Stability
Clock frequency stability. A lower value represents better stability.
Clock precision
Root delay
Root dispersion
Maximum error of the system clock relative to the primary reference source, in milliseconds.
Reference time
Reference timestamp.
display ntp-service trace
Use display ntp-service trace to display brief information about each NTP server from the local device back to the primary reference source.
display ntp-service trace [ source interface-type interface-number ]
source interface-type interface-number: Specifies the source interface for sending NTP packets to trace each NTP server from the local device back to the primary reference source. The source IP address of the NTP packets is the IPv4 address/IPv6 address of the specified source interface. If the IP address of an NTP server is a link-local address, the link-local address of the outgoing interface of NTP packets is used as the source IP address of the NTP packets. If you do not specify this option, the interface that sends the tracing NTP packets acts as the source interface.
To trace back to the primary reference source from the source interface, make sure the source interface and the NTP servers from the local device to the primacy reference source are reachable to each other.
# Display brief information about each NTP server from the local device back to the primary reference source.
<Sysname> display ntp-service trace
Server     127.0.0.1
Stratum    3, jitter  0.000, synch distance 0.0000.
Server     3000::32
Stratum    2 , jitter 790.00, synch distance 0.0000.
RefID      127.127.1.0
The output shows that server 127.0.0.1 is synchronized to server 3000::32, and server 3000::32 is synchronized to the local clock.
Table 6 Command output
Server
Stratum
Stratum level of the NTP server.
jitter
Root mean square (RMS) value of the clock offset relative to the upper-level clock, in seconds.
synch distance
Synchronization distance relative to the upper-level NTP server, in seconds, calculated from dispersion and roundtrip delay values.
RefID
Identifier of the primary reference source. When the stratum level of the primary reference clock is 0, it is displayed as LOCL. Otherwise, it is displayed as the IP address of the primary reference clock.
ntp-service ipv6 source
ntp-service ipv6 unicast-server
ntp-service ipv6 unicast-peer
ntp-service source
ntp-service unicast-server
ntp-service unicast-peer
ntp-service acl
Use ntp-service acl to configure the access-control right for peer devices to access NTP services of the local device.
Use undo ntp-service acl to remove the configured NTP service access-control right.
ntp-service { peer | query | server | synchronization } acl acl-number
undo ntp-service { peer | query | server | synchronization } acl acl-number
The access-control right for the peer devices to access the NTP services of the local device is peer.
peer: Allows time requests and NTP control queries (such as alarms, authentication status, and time server information) from a peer device and allows the local device to synchronize itself to a peer device.
query: Allows only NTP control queries from a peer device to the local device.
server: Allows time requests and NTP control queries from a peer device, but does not allow the local device to synchronize itself to a peer device.
synchronization: Allows only time requests from a peer device.
acl acl-number: Specifies an ACL. The peer devices that match the ACL have the access right specified in the command. The acl-number argument represents a basic ACL number in the range of 2000 to 2999.
You can control NTP access by using ACL. The access rights are in the following order, from least restrictive to most restrictive: peer, server, synchronization, and query.
The device processes an NTP request by following these rules:
·     If no NTP access control is configured, peer is granted to the local device and peer devices.
·     If the IP address of the peer device matches a permit statement in an ACL for more than one access right, the least restrictive access right is granted to the peer device. If a deny statement or no ACL is matched, no access right is granted.
·     If no ACL is created for an access right, the associated access right is not granted.
·     If no ACL is created for any access right, peer is granted.
The ntp-service acl command provides minimal security for a system running NTP. A more secure method is NTP authentication.
# Configure the peer devices on subnet 10.10.0.0/16 to have full access to the local device.
[Sysname] acl basic 2001
[Sysname-acl-ipv4-basic-2001] rule permit source 10.10.0.0 0.0.255.255
[Sysname] ntp-service peer acl 2001
ntp-service authentication enable
ntp-service authentication-keyid
ntp-service reliable authentication-keyid
Use ntp-service authentication enable to enable NTP authentication.
Use undo ntp-service authentication enable to disable NTP authentication.
NTP authentication is disabled.
Enable NTP authentication in networks that require time synchronization security to make sure NTP clients are synchronized only to authenticated NTP servers.
To authenticate an NTP server, set an authentication key and specify it as a trusted key.
# Enable NTP authentication.
[Sysname] ntp-service authentication enable
Use ntp-service authentication-keyid to set an NTP authentication key.
Use undo ntp-service authentication-keyid to remove an NTP authentication key.
ntp-service authentication-keyid keyid authentication-mode { hmac-sha-1 | hmac-sha-256 | hmac-sha-384 | hmac-sha-512 | md5 } { cipher | simple } string
undo ntp-service authentication-keyid keyid
No NTP authentication key exists.
keyid: Specifies an authentication key ID in the range of 1 to 4294967295.
authentication-mode: Specifies an authentication algorithm.
·     hmac-sha-1: Specifies the HMAC-SHA-1 algorithm.
·     hmac-sha-256: Specifies the HMAC-SHA-256 algorithm.
·     hmac-sha-384: Specifies the HMAC-SHA-384 algorithm.
·     hmac-sha-512: Specifies the HMAC-SHA-512 algorithm.
·     md5: Specifies the md5 algorithm.
cipher: Specifies an authentication key in encrypted form.
simple: Specifies an authentication key in plaintext form. For security purposes, the authentication key specified in plaintext form will be stored in encrypted form.
string: Specifies a case-sensitive authentication key. Its plaintext form is a string of 1 to 32 characters. Its encrypted form is a string of 1 to 73 characters.
In a network where there is a high security demand, the NTP authentication feature must be enabled for a system running NTP. This feature enhances the network security by using client-server key authentication, which prohibits a client from synchronizing to a device that has failed the authentication.
Configure the same key ID and key on the client and server.
After you specify an NTP authentication key, use the ntp-service reliable authentication-keyid command to configure the key as a trusted key. The key automatically changes to untrusted after you delete the key. In this case, you do not need to execute the undo ntp-service reliable authentication-keyid command.
The security strength of the five algorithms is HMAC-SHA-512, HMAC-SHA-384, HMAC-SHA-256, HMAC-SHA-1, and MD5 in descending order.
You can set a maximum of 128 authentication keys by executing the command.
# Set a plaintext MD5 authentication key, with the key ID of 10 and key value of BetterKey.
[Sysname] ntp-service authentication-keyid 10 authentication-mode md5 simple BetterKey
ntp-service broadcast-client
Use ntp-service broadcast-client to configure the device to operate in NTP broadcast client mode and use the current interface to receive NTP broadcast packets.
Use undo ntp-service broadcast-client to remove the configuration.
The device does not operate in any NTP association mode.
Interface view
After you configure the command, the device listens to NTP messages sent by the NTP broadcast server and is synchronized based on the received NTP messages.
If you have configured the device to operate in broadcast client mode on an interface with the command, do not add the interface to any aggregate group. To add the interface to an aggregate group, remove the configuration of the command.
# Configure the device to operate in broadcast client mode and receive NTP broadcast messages on VLAN-interface 1.
[Sysname-Vlan-interface1] ntp-service broadcast-client
ntp-service broadcast-server
Use ntp-service broadcast-server to configure the device to operate in NTP broadcast server mode and use the current interface to send NTP broadcast packets.
Use undo ntp-service broadcast-server to remove the configuration.
Interface view
authentication-keyid keyid: Specifies the key ID to be used for sending broadcast messages to broadcast clients. The value range for the keyid argument is 1 to 4294967295. If you do not specify this option, the local device cannot synchronize broadcast clients enabled with NTP authentication.
version number: Specifies the NTP version. The value range for the number argument is 1 to 4, and the default is 4.
After you configure the command, the device periodically sends NTP messages to the broadcast address 255.255.255.255.
If you have configured the device to operate in broadcast server mode on an interface with the command, do not add the interface to any aggregate group. To add the interface to an aggregate group, remove the configuration of the command.
# Configure the device to operate in broadcast server mode and send NTP broadcast messages on VLAN-interface 1, using key 4 for encryption. Set the NTP version to 4.
[Sysname-Vlan-interface1] ntp-service broadcast-server authentication-keyid 4 version 4
ntp-service dscp
Use ntp-server dscp to set a DSCP value for IPv4 NTP packets.
Use undo ntp-server dscp to restore the default.
ntp-service dscp dscp-value
undo ntp-service dscp
The DSCP value for IPv4 NTP packets is 48.
dscp-value: Sets a DSCP value in the range of 0 to 63 for IPv4 NTP packets.
The DSCP value is included in the ToS field of an IPv4 packet to identify the packet priority.
# Set the DSCP value for IPv4 NTP packets to 30.
[Sysname] ntp-service dscp 30
ntp-service enable
Use ntp-service enable to enable the NTP service.
Use undo ntp-service enable to disable the NTP service.
ntp-service enable
The NTP service is disabled.
# Enable the NTP service.
[Sysname] ntp-service enable
ntp-service inbound enable
Use ntp-service inbound enable to enable an interface to receive NTP messages.
Use undo ntp-service inbound enable to disable an interface from receiving NTP messages.
An interface receives NTP messages.
Interface view
Execute the undo ntp-service inbound enable command on an interface in the following cases:
·     You do not want the interface to synchronize the peer device in the corresponding subnet.
·     You do not want the device to be synchronized by the peer device in the subnet corresponding to the interface.
# Disable VLAN-interface 1 from receiving NTP messages.
[Sysname-Vlan-interface1] undo ntp-service inbound enable
ntp-service ipv6 acl
Use ntp-service ipv6 acl to configure the access-control right for the peer devices to access the IPv6 NTP services of the local device.
Use undo ntp-service ipv6 acl to remove the configured NTP service access-control right.
ntp-service ipv6 { peer | query | server | synchronization } acl ipv6-acl-number
undo ntp-service ipv6 { peer | query | server | synchronization } acl ipv6-acl-number
The access-control right for the peer devices to access the IPv6 NTP services of the local device is peer.
Predefined user roes
peer: Allows time requests and NTP control queries (such as alarms, authentication status, and time server information) and allows the local device to synchronize itself to a peer device.
server: Allows time requests and NTP control queries, but does not allow the local device to synchronize itself to a peer device.
synchronization: Allows only time requests from a system whose address passes the access list criteria.
ipv6-acl-number: Specifies an ACL. The peer devices that match the ACL have the access right specified in the command. The ipv6-acl-number argument represents a basic ACL number in the range of 2000 to 2999.
You can control IPv6 NTP access by using ACL. The access rights are in the following order, from least restrictive to most restrictive: peer, server, synchronization, and query.
The ntp-service ipv6 acl command provides a minimum security method. NTP authentication is more secure.
# Configure the peer devices on subnet 2001::1 to have full access to the local device.
[Sysname] acl ipv6 basic 2001
[Sysname-acl-ipv6-basic-2001] rule permit source 2001::1 64
[Sysname] ntp-service ipv6 peer acl 2001
ntp-service ipv6 dscp
Use ntp-server ipv6 dscp to set a DSCP value for IPv6 NTP packets.
Use undo ntp-server ipv6 dscp to restore the default.
ntp-service ipv6 dscp dscp-value
undo ntp-service ipv6 dscp
The DSCP value for IPv6 NTP packets is 56.
dscp-value: Specifies a DSCP value in the range of 0 to 63 for IPv6 NTP packets.
The DSCP value is included in the Traffic Class field of an IPv6 packet to identify the packet priority.
# Set the DSCP value for IPv6 NTP packets to 30.
[Sysname] ntp-service ipv6 dscp 30
ntp-service ipv6 inbound enable
Use ntp-service ipv6 inbound enable to enable an interface to receive IPv6 NTP messages.
Use undo ntp-service ipv6 inbound enable to disable an interface from receiving IPv6 NTP messages.
An interface receives IPv6 NTP messages.
Interface view
Execute the undo ntp-service ipv6 inbound enable command on an interface in the following cases:
·     You do not want the interface to synchronize the peer devices in the corresponding subnet.
·     You do not want the device to be synchronized by the peer devices in the subnet corresponding to the interface.
# Disable VLAN-interface 1 from receiving IPv6 NTP messages.
[Sysname-Vlan-interface1] undo ntp-service ipv6 inbound enable
ntp-service ipv6 multicast-client
Use ntp-service ipv6 multicast-client to configure the device to operate in IPv6 NTP multicast client mode and use the current interface to receive IPv6 NTP multicast packets.
Use undo ntp-service ipv6 multicast-client to remove the configuration.
ntp-service ipv6 multicast-client ipv6-address
undo ntp-service ipv6 multicast-client ipv6-address
Interface view
ipv6-address: Specifies an IPv6 multicast address. An IPv6 broadcast client and an IPv6 broadcast server must be configured with the same multicast address.
After you configure the command, the device listens to IPv6 NTP messages using the specified multicast address as the destination address. It is synchronized based on the received IPv6 NTP messages.
If you have configured the device to operate in IPv6 multicast client mode on an interface by using the command, do not add the interface to any aggregate group. To add the interface to an aggregate group, remove the configuration of the command.
# Configure the device to operate in IPv6 multicast client mode and receive IPv6 NTP multicast messages with the destination FF21::1 on VLAN-interface 1.
[Sysname-Vlan-interface1] ntp-service ipv6 multicast-client ff21::1
ntp-service ipv6 multicast-server
Use ntp-service ipv6 multicast-server to configure the device to operate in IPv6 NTP multicast server mode and use the current interface to send IPv6 NTP multicast packets.
Use undo ntp-service ipv6 multicast-server to remove the configuration.
ntp-service ipv6 multicast-server ipv6-address [ authentication-keyid keyid | ttl ttl-number ] *
undo ntp-service ipv6 multicast-server ipv6-address
Interface view
ipv6-address: Specifies an IPv6 multicast address. An IPv6 multicast client and server must be configured with the same multicast address.
authentication-keyid keyid: Specifies the key ID to be used for sending multicast messages to multicast clients. The value range for the keyid argument is 1 to 4294967295. If you do not specify this option, the local device cannot synchronize clients enabled with NTP authentication.
ttl ttl-number: Specifies the TTL of NTP multicast messages. The value range for the ttl-number argument is 1 to 255, and the default is 16.
After you configure the command, the device periodically sends NTP messages to the specified IPv6 multicast address.
If you have configured the device to operate in IPv6 multicast server mode on an interface with the command, do not add the interface to any aggregate group. To add the interface to an aggregate group, remove the configuration of the command.
# Configure the device to operate in IPv6 multicast server mode and send IPv6 NTP multicast messages on VLAN-interface 1 to the multicast address FF21::1, using key 4 for encryption.
[Sysname-Vlan-interface1] ntp-service ipv6 multicast-server ff21::1 authentication-keyid 4
Use ntp-service ipv6 source to specify a source interface for IPv6 NTP messages.
Use undo ntp-service ipv6 source to restore the default.
ntp-service ipv6 source interface-type interface-number
No source interface is specified for IPv6 NTP messages. The device automatically selects the source IP address for IPv6 NTP messages. For more information, see RFC 3484.
If you specify a source interface for IPv6 NTP messages, the device uses the IPv6 address of the source interface as the source address to send IPv6 NTP messages. Consequently, the destination address of the IPv6 NTP response messages is the address of the source interface.
When the device responds to an IPv6 NTP request, the source IPv6 address of the NTP response is always the IPv6 address of the interface that has received the IPv6 NTP request.
If you do not want the IPv6 address of an interface on the local device to become the destination address for response messages, use the command to specify another interface as the source interface for IPv6 NTP messages.
The source interface for IPv6 NTP messages can also be specified in the following ways:
·     In NTP client/server mode, if you have specified the source interface for IPv6 NTP messages in the ntp-service ipv6 unicast-server command, the specified interface acts as the source interface for IPv6 NTP messages.
·     In NTP symmetric active/passive mode, if you have specified the source interface for IPv6 NTP messages in the ntp-service ipv6 unicast-peer command, the specified interface acts as the source interface for IPv6 NTP messages.
·     In NTP multicast mode, if you have configured the ntp-service ipv6 multicast-server command on an interface, the interface acts as the source interface for NTP multicast messages.
If the specified source interface is down, the device does not send IPv6 NTP messages.
# Specify the source interface of IPv6 NTP messages as VLAN-interface 1.
[Sysname] ntp-service ipv6 source vlan-interface 1
Use ntp-service ipv6 unicast-peer to specify an IPv6 symmetric-passive peer for the device.
Use undo ntp-service ipv6 unicast-peer to remove the IPv6 symmetric-passive peer specified for the device.
ntp-service ipv6 unicast-peer { peer-name | ipv6-address } [ vpn-instance vpn-instance-name ] [ authentication-keyid keyid | priority | source interface-type interface-number ] *
undo ntp-service ipv6 unicast-peer { peer-name | ipv6-address } [ vpn-instance vpn-instance-name ]
No IPv6 symmetric-passive peer is specified.
peer-name: Specifies a symmetric-passive peer by its host name, a case-insensitive string of 1 to 253 characters.
ipv6-address: Specifies a symmetric-passive peer by its IPv6 address. It must be a unicast address, rather than a multicast address.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the symmetric-passive peer belongs. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If the symmetric-passive peer is on the public network, do not specify this option.
authentication-keyid keyid: Specifies the key ID to be used for sending NTP messages to the peer. The value range for the keyid argument is 1 to 4294967295. If you do not specify this option, the local device and the peer do not authenticate each other.
priority: Specifies the peer specified by ipv6-address or peer-name as the first choice under the same condition.
source interface-type interface-number: Specifies the source interface for IPv6 NTP messages. If the specified passive peer address is not a link local address, the source IPv6 address for IPv6 NTP messages sent by the local device is the IPv6 address of the specified source interface. If the specified passive peer address is a link local address, the IPv6 NTP messages are sent from the specified source interface, and the source address of the messages is the link local address of the interface. The interface-type interface-number argument represents the interface type and number. If you do not specify an interface, the device automatically selects the source IPv6 address of IPv6 NTP messages. For more information, see RFC 3484.
When you specify an IPv6 passive peer for the device, the device and its IPv6 passive peer can be synchronized to each other. If their clocks are in synchronized state, the clock with a high stratum level is synchronized to the clock with a lower stratum level.
To synchronize the PE to a PE or CE in a VPN instance, provide the vpn-instance vpn-instance-name option in the command.
If you include the vpn-instance vpn-instance-name option in the undo ntp-service ipv6 unicast-peer command, the command removes the symmetric-passive peer in the specified VPN instance. If you do not include the vpn-instance vpn-instance-name option in the command, the command removes the symmetric-passive peer on the public network.
If the specified IPv6 address of the passive peer is a link local address, you must specify the source interface for NTP messages and cannot specify a VPN instance for the passive peer.
# Specify the device with the IPv6 address of 2001::1 as the symmetric-passive peer of the device, and specify the source interface for IPv6 NTP messages as VLAN-interface 1.
[Sysname] ntp-service ipv6 unicast-peer 2001::1 source vlan-interface 1
Use ntp-service ipv6 unicast-server to specify an IPv6 NTP server for the device.
Use undo ntp-service ipv6 unicast-server to remove an IPv6 NTP server specified for the device.
ntp-service ipv6 unicast-server { server-name | ipv6-address } [ vpn-instance vpn-instance-name ] [ authentication-keyid keyid | priority | source interface-type interface-number ] *
undo ntp-service ipv6 unicast-server { server-name | ipv6-address } [ vpn-instance vpn-instance-name ]
No IPv6 NTP server is specified.
server-name: Specifies an NTP server by its host name, a case-insensitive string of 1 to 253 characters.
ipv6-address: Specifies an NTP server by its IPv6 address. It must be a unicast address, rather than a multicast address.
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance to which the NTP server belongs. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If the NTP server is on the public network, do not specify this option.
authentication-keyid keyid: Specifies the key ID to be used for sending NTP messages to the NTP server. The value range for the keyid argument is 1 to 4294967295. If you do not specify this option, the local device and NTP server do not authenticate each other.
priority: Specifies this NTP server as the first choice under the same condition.
source interface-type interface-number: Specifies the source interface for IPv6 NTP messages. If the specified IPv6 NTP server address is not a link local address, the source IPv6 address for IPv6 NTP messages sent by the local device to the NTP server is the IPv6 address of the specified source interface. If the specified IPv6 NTP server address is a link local address, the IPv6 NTP messages are sent from the specified source interface, and the source address of the messages is the link local address of the interface. The interface-type interface-number argument represents the interface type and number. If you do not specify an interface, the device automatically selects the source IPv6 address of IPv6 NTP messages. For more information, see RFC 3484.
When you specify an IPv6 NTP server for the device, the device is synchronized to the IPv6 NTP server, but the IPv6 NTP server is not synchronized to the device.
To synchronize the PE to a PE or CE in a VPN instance, specify the vpn-instance vpn-instance-name option in the command.
If you include the vpn-instance vpn-instance-name option in the undo ntp-service unicast-server command, the command removes the NTP server in the specified VPN. If you do not include the vpn-instance vpn-instance-name option in the command, the command removes the NTP server on the public network.
If the specified IPv6 address of the NTP server is a link local address, you must specify the source interface for NTP messages and cannot specify a VPN instance for the NTP server.
# Specify the IPv6 NTP server 2001::1 for the device.
[Sysname] ntp-service ipv6 unicast-server 2001::1
ntp-service max-dynamic-sessions
Use ntp-service max-dynamic-sessions to set the maximum number of dynamic NTP sessions.
Use undo ntp-service max-dynamic-sessions to restore the default.
The maximum number of dynamic NTP sessions is 100.
number: Sets the maximum number of dynamic NTP associations, in the range of 0 to 100.
A device can have a maximum of 128 concurrent associations, including static associations and dynamic associations. A static association refers to an association that a user has manually created by using an NTP command. A dynamic association is a temporary association created by the system during operation.
This command limits the number of dynamic NTP associations and prevents dynamic NTP associations from occupying too many system resources.
# Set the maximum number of dynamic NTP associations to 50.
[Sysname] ntp-service max-dynamic-sessions 50
ntp-service multicast-client
Use ntp-service multicast-client to configure the device to operate in NTP multicast client mode and use the current interface to receive NTP multicast packets.
Use undo ntp-service multicast-client to remove the configuration.
undo ntp-service multicast-client [ ip-address ]
Interface view
ip-address: Specifies a multicast IP address. The default is 224.0.1.1. A multicast server and client must be configured with the same multicast IP address.
After you configure the command, the device listens to NTP messages using the specified multicast address as the destination address.
If you have configured the device to operate in multicast client mode on an interface with the command, do not add the interface to any aggregate group. To add the interface to an aggregate group, remove the configuration of the command.
# Configure the device to operate in multicast client mode and receive NTP multicast messages on VLAN-interface 1, and set the multicast address to 224.0.1.1.
[Sysname-Vlan-interface1] ntp-service multicast-client 224.0.1.1
ntp-service multicast-server
Use ntp-service multicast-server to configure the device to operate in NTP multicast server mode and use the current interface to send NTP multicast packets.
Use undo ntp-service multicast-server to remove the configuration.
undo ntp-service multicast-server [ ip-address ]
Interface view
authentication-keyid keyid: Specifies the key ID to be used for sending multicast messages to multicast clients. The value range for the keyid argument is 1 to 4294967295. If you do not specify this option, the local device cannot synchronize multicast clients enabled with NTP authentication.
ttl ttl-number: Specifies the TTL of NTP multicast messages. The value range for the ttl-number argument is 1 to 255. The default value is 16.
version number: Specifies the NTP version. The value range for the number argument is 1 to 4. The default value is 4.
After you configure the command, the device periodically sends NTP messages to the specified multicast address.
If you have configured the device to operate in multicast server mode on an interface with the command, do not add the interface to any aggregate group. To add the interface to an aggregate group, remove the configuration of the command.
# Configure the device to operate in multicast server mode and send NTP multicast messages on VLAN-interface 1 to the multicast address 224.0.1.1, using key 4 for encryption. Set the NTP version to 4.
[Sysname-Vlan-interface1] ntp-service multicast-server 224.0.1.1 version 4 authentication-keyid 4
Use ntp-service refclock-master to configure the local clock as the reference source.
Use undo ntp-service refclock-master to remove the configuration.
undo ntp-service refclock-master [ ip-address ]
The device does not use its local clock as the reference clock.
ip-address: IP address of the local clock, 127.127.1.u, where u is the NTP process ID in the range of 0 to 3. The default value is 127.127.1.0.
stratum: Stratum level of the local clock, in the range of 1 to 15. The default value is 8. A lower stratum level represents higher clock accuracy.
Typically an NTP server that gets its time from an authoritative time source, such as an atomic clock has stratum 1 and operates as the primary time server to provide time synchronization for other devices in the network. The accuracy of each server is the stratum, with the topmost level (primary servers) assigned as one and each level downwards (secondary servers) in the hierarchy assigned as one greater than the preceding level.
If the devices in a network cannot synchronize to an authoritative time source, you can perform the following tasks:
·     Select a device that has a relatively accurate clock from the network.
·     Use the local clock of the device as the reference clock to synchronize other devices in the network.
Use the command with caution to avoid time errors. As a best practice, set the local clock time to a correct value before you execute the command.
# Specify the local clock as the reference source, with the stratum level 2.
[Sysname] ntp-service refclock-master 2
Use ntp-service reliable authentication-keyid to specify an authentication key as a trusted key.
Use undo ntp-service reliable authentication-keyid to remove the configuration.
undo ntp-service reliable authentication-keyid keyid
No trusted key is specified.
keyid: Specifies an authentication key by its ID in the range of 1 to 4294967295.
When NTP authentication is enabled, a client can be synchronized only to a server that can provide a trusted authentication key.
Before you use the command, make sure NTP authentication is enabled and an authentication key is configured. The key automatically changes to untrusted after you delete the key. In this case, you do not need to execute the undo ntp-service reliable authentication-keyid command.
You can set a maximum of 128 keys by executing the command.
# Enable NTP authentication, specify the MD5 algorithm, with the key ID of 37 and key value of BetterKey.
[Sysname] ntp-service authentication-keyid 37 authentication-mode md5 simple BetterKey
# Specify this key as a trusted key.
[Sysname] ntp-service reliable authentication-keyid 37
ntp-service source
Use ntp-service source to specify a source interface for NTP messages.
Use undo ntp-service source to restore the default.
ntp-service source interface-type interface-number
No source interface is specified for NTP messages. The device performs the following operations:
·     Searches the routing table for the outbound interface of NTP messages.
·     Uses the primary IP address of the outbound interface as the source IP address for NTP messages.
If you specify a source interface for NTP messages, the device uses the primary IP address of the specified interface as the source IP address to send NTP messages. Consequently, the destination address of the NTP response messages is the primary IP address of the source interface.
When the device responds to an NTP request, the source IP address of the NTP response is always the IP address of the interface that has received the NTP request.
If you do not want the IP address of an interface on the local device to become the destination address for response messages, use the command to specify another interface as the source interface for NTP messages.
The source interface for NTP messages can also be specified in the following ways:
·     In NTP client/server mode, if you have specified the source interface for NTP messages in the ntp-service unicast-server command, the specified interface acts as the source interface for NTP messages.
·     In NTP symmetric active/passive mode, if you have specified the source interface for NTP messages in the ntp-service unicast-peer command, the specified interface acts as the source interface for NTP messages.
·     In NTP multicast mode, if you have configured the ntp-service multicast-server command on an interface, the interface acts as the source interface for NTP multicast messages.
·     In NTP broadcast mode, if you have configured the ntp-service broadcast-server command on an interface, the interface acts as the source interface for NTP broadcast messages.
If the specified source interface is down, the device does not send NTP messages.
# Specify the source interface for NTP messages as VLAN-interface 1.
[Sysname] ntp-service source vlan-interface 1
Use ntp-service unicast-peer to specify a symmetric-passive peer for the device.
Use undo ntp-service unicast-peer to remove the symmetric-passive peer specified for the device.
ntp-service unicast-peer { peer-name | ip-address } [ vpn-instance vpn-instance-name ] [ authentication-keyid keyid | priority | source interface-type interface-number | version number ] *
undo ntp-service unicast-peer { peer-name | ip-address } [ vpn-instance vpn-instance-name ]
No symmetric-passive peer is specified.
ip-address: Specifies a symmetric-passive peer by its IP address. It must be a unicast address, rather than a broadcast address, a multicast address, or the IP address of the local clock.
priority: Specifies the peer specified by ip-address or peer-name as the first choice under the same condition.
source interface-type interface-number: Specifies the source interface for NTP messages. In an NTP message the local device sends to its peer, the source IP address is the primary IP address of this interface. The interface-type interface-number argument represents the interface type and number. If you do not specify this option, the device searches the routing table for the outgoing interface and uses the primary IP address of the outgoing interface as the source IP address of the NTP messages.
When you specify a passive peer for the device, the device and its passive peer can be synchronized to each other. If their clocks are in synchronized state, the clock with a high stratum level is synchronized to the clock with a lower stratum level.
To synchronize the PE to a PE or CE in a VPN instance, provide vpn-instance vpn-instance-name in your command.
If you include vpn-instance vpn-instance-name in the undo ntp-service unicast-peer command, the command removes the symmetric-passive peer in the specified VPN instance. If you do not include vpn-instance vpn-instance-name in the command, the command removes the symmetric-passive peer on the public network.
# Specify the device with the IP address of 10.1.1.1 as the symmetric-passive peer of the device, and configure the device to run NTP version 4. Specify the source interface of NTP messages as VLAN-interface 1.
[Sysname] ntp-service unicast-peer 10.1.1.1 version 4 source-interface vlan-interface 1
Use ntp-service unicast-server to specify an NTP server for the device.
Use undo ntp-service unicast-server to remove an NTP server specified for the device.
ntp-service unicast-server { server-name | ip-address } [ vpn-instance vpn-instance-name ] [ authentication-keyid keyid | priority | source interface-type interface-number | version number ] *
undo ntp-service unicast-server { server-name | ip-address } [ vpn-instance vpn-instance-name ]
No NTP server is specified.
ip-address: Specifies an NTP server by its IP address. It must be a unicast address, rather than a broadcast address, a multicast address, or the IP address of the local clock.
source interface-type interface-number: Specifies the source interface for NTP messages. For an NTP message the local device sends to the NTP server, the source IP address is the primary IP address of this interface. The interface-type interface-number argument represents the interface type and number. If you do not specify this option, the device searches the routing table for the outgoing interface and uses the primary IP address of the outgoing interface as the source IP address of the NTP messages.
When you specify an NTP server for the device, the device is synchronized to the NTP server, but the NTP server is not synchronized to the device.
If you include the vpn-instance vpn-instance-name option in the undo ntp-service unicast-server command, the command removes the NTP server in the specified VPN instance. If you do not include the vpn-instance vpn-instance-name option in the command, the command removes the NTP server on the public network.
# Specify NTP server 10.1.1.1 for the device, and configure the device to run NTP version 4.
[Sysname] ntp-service unicast-server 10.1.1.1 version 4
SNTP commands
display sntp ipv6 sessions
Use display sntp ipv6 sessions to display information about all IPv6 SNTP associations.
# Display information about all IPv6 SNTP associations.
<Sysname> display sntp ipv6 sessions
SNTP server: 2001::1
Stratum: 16
Version: 4
Last receive time: No packet was received.
SNTP server: 2001::100
Stratum: 3
Version: 4
Last receive time: Fri, Oct 21 2011 11:28:28.058 (Synced)
Table 7 Command output
SNTP server
SNTP server (NTP server). If this field displays ::, the IPv6 address of the NTP server has not been resolved successfully.
Stratum
Stratum level of the NTP server, which determines the clock accuracy. It is in the range of 1 to 16. A lower stratum level represents a higher clock accuracy. A clock with stratum level 16 is not synchronized.
Version
SNTP version.
Last receive time
Time when the last message was received:
·     Synced—The local clock is synchronized to the NTP server.
·     No packet was received—The device has not received any SNTP session information from the server.
display sntp sessions
Use display sntp sessions to display information about all IPv4 SNTP associations.
# Display information about all IPv4 SNTP associations.
<Sysname> display sntp sessions
SNTP server     Stratum   Version    Last receive time
1.0.1.11        2         4          Tue, May 17 2011  9:11:20.833 (Synced)
Table 8 Command output
SNTP server
SNTP server (NTP server). If this field displays 0.0.0.0, the IP address of the NTP server has not been resolved successfully.
Stratum
Stratum level of the NTP server, which determines the clock accuracy. It is in the range of 1 to 16. A lower stratum level represents higher clock accuracy. A clock with stratum level 16 is not synchronized.
Version
SNTP version.
Last receive time
Time when the last message was received. Synced means the local clock is synchronized to the NTP server.
sntp authentication enable
Use sntp authentication enable to enable SNTP authentication.
Use undo sntp authentication enable to disable SNTP authentication.
SNTP authentication is disabled.
You need to enable SNTP authentication in networks that require time synchronization security to make sure SNTP clients are synchronized only to authenticated NTP servers.
# Enable SNTP authentication.
[Sysname] sntp authentication enable
sntp authentication-keyid
sntp reliable authentication-keyid
Use sntp authentication-keyid to set an SNTP authentication key.
Use undo sntp authentication-keyid to remove an SNTP authentication key.
sntp authentication-keyid keyid authentication-mode { hmac-sha-1 | hmac-sha-256 | hmac-sha-384 | hmac-sha-512 | md5 } { cipher | simple } string
undo sntp authentication-keyid keyid
No SNTP authentication key exists.
Configure the same key ID and key on the SNTP client and NTP server. Otherwise, the SNTP client cannot be synchronized to the NTP server.
After you configure an SNTP authentication key, use the sntp reliable authentication-keyid command to set it as a trusted key. The key automatically changes to untrusted after you delete the key. In this case, you do not need to execute the undo sntp-service reliable authentication-keyid command.
# Set an MD5 authentication key, with the key ID of 10 and key value of BetterKey. Input the key in plain text.
[Sysname] sntp authentication-keyid 10 authentication-mode md5 simple BetterKey
sntp enable
Use sntp enable to enable the SNTP service.
Use undo sntp enable to disable the SNTP service.
sntp enable
undo sntp enable
The SNTP service is disabled.
# Enable the SNTP service.
[Sysname] sntp enable
sntp ipv6 unicast-server
Use sntp ipv6 unicast-server to specify an IPv6 NTP server for the device.
Use undo sntp ipv6 unicast-server to remove the IPv6 NTP server specified for the device.
sntp ipv6 unicast-server { server-name | ipv6-address } [ vpn-instance vpn-instance-name ] [ authentication-keyid keyid | source interface-type interface-number ] *
undo sntp ipv6 unicast-server { server-name | ipv6-address } [ vpn-instance vpn-instance-name ]
vpn-instance vpn-instance-name: Specifies MPLS L3VPN instance to which the NTP server belongs. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If the NTP server is on the public network, do not specify this option.
When you specify an IPv6 NTP server for the device, the device is synchronized to the NTP server, but the NTP server is not synchronized to the device.
To synchronize the PE to a PE or CE in a VPN instance, provide the vpn-instance vpn-instance-name option in your command.
[Sysname] sntp ipv6 unicast-server 2001::1
Use sntp reliable authentication-keyid to specify a trusted key.
Use undo sntp reliable authentication-keyid to remove the trusted key.
sntp reliable authentication-keyid keyid
undo sntp reliable authentication-keyid keyid
If SNTP is enabled, the SNTP client is synchronized only to an NTP server that provides a trusted key.
Before you use the command, make sure SNTP authentication is enabled and an authentication key is configured. The key automatically changes to untrusted after you delete the key. In this case, you do not need to execute the undo sntp-service reliable authentication-keyid command.
# Enable NTP authentication, and specify the MD5 encryption algorithm, with the key ID of 37 and key value of BetterKey.
[Sysname] sntp authentication-keyid 37 authentication-mode md5 simple BetterKey
[Sysname] sntp reliable authentication-keyid 37
sntp unicast-server
Use sntp unicast-server to specify an NTP server for the device.
Use undo sntp unicast-server to remove an NTP server specified for the device.
sntp unicast-server { server-name | ip-address } [ vpn-instance vpn-instance-name ] [ authentication-keyid keyid | source interface-type interface-number | version number ] *
undo sntp unicast-server { server-name | ip-address } [ vpn-instance vpn-instance-name ]
vpn-instance vpn-instance-name: Specifies the MPLS L3VPN instance VPN to which the NTP server belongs. The vpn-instance-name argument is a case-sensitive string of 1 to 31 characters. If the NTP server is on the public network, do not specify this option.
source interface-type interface-number: Specifies the source interface for NTP messages. In an NTP message the local device sends to the NTP server, the source IP address is the primary IP address of this interface. The interface-type interface-number argument represents the interface type and number.
[Sysname] sntp unicast-server 10.1.1.1 version 4