H3C Data Center Switches DRNI Configuration Guide-6W103
HomeSupportConfigure & DeployConfiguration GuidesH3C Data Center Switches DRNI Configuration Guide-6W103
13-DRNI and MVXLAN Configuration Example
13-DRNI and MVXLAN Configuration Example 251.12 KB
Example: Configuring DRNI with MDT-based MVXLAN
As shown in Figure 1:
·     Switch A, Switch B, Switch C, Switch D, and Switch E are distributed EVPN gateways.
¡     Leaf devices Switch A and Switch B form a DR system through DRNI, and they use the IPL to synchronize MAC and ARP entries to ensure MAC and ARP entry consistency. In this example, an Ethernet aggregate link acts as the IPL.
¡     Switch C and Switch D form a DR system through DRNI, and the DR system acts all the roles of spine, border, and leaf. In this example, an Ethernet aggregate link acts as the IPL.
¡     Switch E acts as a standalone leaf device.
·     Switch A and Switch B are connected to VM 1 and VM 2 through Ethernet links. On Switch A and Switch B, the Ethernet links connected to the same VM are aggregated into a Layer 2 aggregation group to avoid single points of failure. Connect Switch C, Switch D, and VMs in the same way Switch A, Switch B, VM 1, and VM 2 are connected.
·     VM 1 is the multicast source. VM 2, VM 3, VM 5, and VM 6 are multicast receivers in a private network. VM 4 is a multicast receiver in the public network. They use MVXLAN to transmit multicast traffic.
Figure 1 Network diagram
Device
IP address
Switch A
Loopback 0
1.1.1.1/32
Loopback 1
1.2.3.4/32
Loopback 2
1.2.3.4/32
HundredGigE 1/0/25
11.1.1.2/24
HundredGigE 1/0/27
12.1.1.2/24
HundredGigE 1/0/30
21.0.0.1/24
VSI-interface 1
10.1.1.1/24
VSI-interface 2
10.1.2.1/24
Switch B
Loopback 0
2.2.2.2/32
Loopback 1
1.2.3.4/32
Loopback 2
1.2.3.4/32
HundredGigE 2/0/25
13.1.1.2/24
HundredGigE 2/0/27
14.1.1.2/24
HundredGigE 2/0/30
21.0.0.2/24
VSI-interface 1
10.1.1.1/24
VSI-interface 2
10.1.2.1/24
Switch C
Loopback 0
4.4.4.4/32
Loopback 1
5.6.7.8/32
Loopback 2
5.6.7.8/32
HundredGigE 1/0/25
11.1.1.1/24
HundredGigE 1/0/27
13.1.1.1/24
HundredGigE 1/0/30
15.1.1.1/24
HundredGigE 1/0/31
21.1.0.1
VSI-interface 1
10.1.1.1/24
VSI-interface 2
10.1.2.1/24
VLAN-interface 100
100.1.1.3/24
Switch D
Loopback 0
5.5.5.5/32
Loopback 1
5.6.7.8/32
Loopback 2
5.6.7.8/32
HundredGigE 1/0/25
12.1.1.1/24
HundredGigE 1/0/27
14.1.1.1/24
HundredGigE 1/0/30
16.1.1.1/24
HundredGigE 1/0/31
21.1.0.2
VSI-interface 1
10.1.1.1/24
VSI-interface 2
10.1.2.1/24
VLAN-interface 100
100.1.1.4/24
Switch E
Loopback 0
3.3.3.3/32
Loopback 1
3.3.3.3/32
HundredGigE 1/0/25
15.1.1.2/24
HundredGigE 1/0/26
16.1.1.2/24
VSI-interface 1
10.1.1.1/24
VSI-interface 2
10.1.2.1/24
Applicable product matrix
IMPORTANT
IMPORTANT:
In addition to running an applicable software version, you must also install the most recent patch, if any.
Device
Software version
S6805, S6825, S6850, and S9850
F6632 and higher F66xx or R66xx versions
S12500G-AF
R7624P12
S6800 and S6860
No versions recommended
S12500X-AF, S6890, S9820-64H, and S9820-8C
Not supported
S6812 and S6813
To be released. To obtain the availability of software, contact H3C Technical Support.
·     The member devices in a DR system must use the same DR system MAC address. Different DR systems must each have a unique DR system MAC address on the network.
·     As a best practice, run a dynamic routing protocol between the spine devices and the external network. If you use static routing, rebooting spine devices might cause traffic interruption. For example, traffic interruption occurs if the service modules that provide IPP member ports, keepalive interfaces, and DR interfaces start up slower than other service modules. To resolve the issue, use one of the following solutions:
¡     Assign ports operating at the same rate to the IPPs on all service modules to ensure that the IPPs are always restored first. If the member ports cannot operate at the same rate, use the link-aggregation ignore speed command on the IPPs to ensure ports at all rates can be selected. In this solution, hash congestion or uneven load sharing might occur.
¡     On the spine devices, configure a monitor link group. To ensure that the uplink interfaces always start up earlier than the downlink DR interfaces, assign all downlink DR member ports to the monitor link group as uplink interfaces and assign all uplink interfaces to the monitor link group as downlink interfaces. The maintainability of this solution is weak. When you add, delete, or modify DR groups, you must update the uplink interfaces of the monitor link group accordingly.
·     All ACs must be dual-homed to the DR member devices. Singlehomed ACs are not supported. Multicast traffic load sharing is not supported. The IPL can only be an Ethernet aggregate link.
·     MVXLAN supports only IPv4 underlay networks and IPv4 overlay networks in the current software version.
·     As a best practice, create frame match criteria based on VXLAN IDs for the dynamic ACs on the IPL.
·     As a best practice to ensure correct traffic forwarding, do not allow IPP s or DR interfaces to forward traffic in the VLANs to which transport-facing interfaces are assigned.
·     When a device plays all roles of leaf, border, and spine, packet loss occurs if the multicast source is on the public network and the receivers are attached to ACs in VPN instances. If such multicast traffic exists, do not configure a device to play all roles of leaf, border, and spine.
Configuring access devices
Procedure summary
·     Configuring access devices Switch A and Switch B
·     Configuring access device Switch E
Switch A
Switch B
ip vpn-instance vpn1
Create VPN instance vpn1.
route-distinguisher 1:1
Configure an RD for the VPN instance.
address-family ipv4
address-family ipv4
Enter VPN instance IPv4 address family view.
vpn-target 2:2
vpn-target 2:2
Configure a route target for the VPN instance.
N/A
address-family evpn
address-family evpn
Enter VPN instance EVPN view.
vpn-target 1:1
vpn-target 1:1
Configure a route target for EVPN.
N/A
N/A
ospf 1 router-id 1.1.1.1
ospf 1 router-id 2.2.2.2
Enable OSPF process 1, specify a route ID, and enter OSPF process view.
stub-router include-stub on-startup 900
Configure the router as a stub router during reboot and specify the timeout time to 900 seconds.
area 0.0.0.0
area 0.0.0.0
Create an OSPF area.
N/A
N/A
interface loopback 0
Create interface Loopback 0.
pim sm
pim sm
Enable PIM SM on the interface.
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
Enable OSPF process 1 on the interface.
N/A
interface loopback 1
Create interface Loopback 1.
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
interface loopback 2
Create interface Loopback 2.
ip binding vpn-instance vpn1
Associate the interface with VPN instance vpn1.
pim sm
pim sm
interface hundredgige 1/0/25
interface hundredgige 2/0/25
Enter interface view.
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
interface hundredgige 1/0/27
interface hundredgige 2/0/27
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
interface hundredgige 1/0/30
interface hundredgige 2/0/30
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
l2vpn enable
l2vpn enable
Enable L2VPN.
Disable remote MAC learning.
vxlan tunnel arp-learning disable
Disable remote ARP learning.
evpn global-mac 0001-0002-0003
Specify a global EVPN MAC address.
vsi vpn1
vsi vpn1
Create VSI vpn1 and enter VSI view.
flooding disable unknown-unicast unknown-multicast
Disable flooding for the VSI.
vxlan 10
vxlan 10
Create VXLAN 10 and enter VXLAN view.
N/A
evpn encapsulation vxlan
Create an EVPN instance.
route-distinguisher auto
Configure the switch to automatically generate an RD for the EVPN instance.
vpn-target auto
vpn-target auto
Configure the switch to automatically generate a route target for the EVPN instance.
N/A
N/A
vsi vpn2
vsi vpn2
Create VSI vpn2 and enter VSI view.
vxlan 20
vxlan 20
Create VXLAN 20 and enter VXLAN view.
N/A
vpn-target auto
vpn-target auto
N/A
N/A
interface vsi-interface 1
Create VSI-interface 1.
Associate the VSI interface with VPN instance vpn1.
mac-address 0001-0001-0001
Specify a MAC address for the VSI interface.
local-proxy-arp enable
Enable local proxy ARP.
distributed-gateway local
Specify the VSI interface as a distributed gateway.
pim distributed-dr
pim distributed-dr
Configure the VSI interface as a distributed designated router interface.
igmp enable
igmp enable
Enable IGMP on the interface.
pim sm
pim sm
N/A
interface vsi-interface 2
Create VSI-interface 2.
mac-address 0002-0002-0002
pim distributed-dr
pim distributed-dr
igmp enable
igmp enable
pim sm
pim sm
N/A
interface vsi-interface 3
Create VSI-interface 3.
pim sm
pim sm
l3-vni 1000
l3-vni 1000
Configure the Layer 3 VXLAN ID as 1000.
N/A
vsi vpn1
vsi vpn1
Enter the view of VSI vpn1.
gateway vsi-interface 1
Specify VSI-interface 1 as the gateway interface for the VSI.
N/A
vsi vpn2
vsi vpn2
Enter the view of VSI vpn2.
gateway vsi-interface 2
Specify VSI-interface 2 as the gateway interface for the VSI.
N/A
l2vpn drni peer-link ac-match-rule vxlan-mapping
Enable the switch to create frame match criteria based on VXLAN IDs for the dynamic ACs on the IPL.
evpn drni group 1.2.3.4
Enable EVPN distributed relay and specify the virtual VTEP address.
evpn drni local 1.1.1.1 remote 2.2.2.2
evpn drni local 2.2.2.2 remote 1.1.1.1
Specify the IP addresses of the local and peer VTEPs in the DR system.
drni restore-delay 300
Set the data restoration interval to 300 seconds.
drni system-mac 0021-0021-0021
Configure the DR system MAC address.
drni system-number 1
drni system-number 2
Set the DR system number.
drni system-priority 21
Set the DR system priority.
drni standalone enable
Enable DRNI standalone mode.
drni keepalive ip destination 21.0.0.2 source 21.0.0.1
drni keepalive ip destination 21.0.0.1 source 21.0.0.2
Configure DR keepalive packet parameters.
interface bridge-aggregation 1
Create Layer 2 aggregate interface Bridge-Aggregation 1 and enter its view.
link-aggregation mode dynamic
Configure the aggregation group to operate in dynamic aggregation mode and enable LACP.
N/A
interface hundredgige 1/0/29
interface hundredgige 2/0/29
port link-aggregation group 1
Assign the interface to aggregation group 1.
N/A
Enter the view of Bridge-Aggregation 1.
port drni intra-portal-port 1
Configure Bridge-Aggregation 1 as the IPP.
undo mac-address static source-check enable
Disable static source check to ensure correct Layer 3 forwarding over the IPL.
N/A
interface bridge-aggregation 2
Create Layer 2 aggregate interface Bridge-Aggregation 2 and enter its view.
port trunk pvid vlan 4040
Configure the Layer 2 aggregate interface as a trunk port and set its PVID to 4040.
N/A
interface hundredgige 1/0/26
interface hundredgige 2/0/26
port link-aggregation group 2
Assign the interface to aggregation group 2.
N/A
Enter the view of Bridge-Aggregation 2.
port link-type trunk
Set the link type of the aggregate interface to trunk.
undo port trunk permit vlan 1
Remove the aggregate interface from VLAN 1.
port trunk permit vlan 2 to 3
Assign the aggregate interface to VLANs 2 and 3.
port drni group 2
port drni group 2
Assign the aggregate interface to DR group 2.
N/A
drni mad exclude interface hundredgige 1/0/25
drni mad exclude interface hundredgige 2/0/25
Exclude an interface from the DRNI MAD shutdown action.
drni mad exclude interface hundredgige 1/0/27
drni mad exclude interface hundredgige 2/0/27
drni mad exclude interface hundredgige 1/0/30
drni mad exclude interface hundredgige 2/0/30
drni mad exclude interface loopback 0
drni mad exclude interface loopback 1
drni mad exclude interface loopback 2
drni mad exclude interface vsi-interface 1
drni mad exclude interface vsi-interface 2
drni mad exclude interface vsi-interface 3
bgp 100
bgp 100
Create BGP instance 100.
router-id 1.1.1.1
router-id 2.2.2.2
Configure a router ID for the BGP instance.
peer 4.4.4.4 as-number 100
Specify an AS number for a peer group.
peer 4.4.4.4 connect-interface loopback 0
Specify a source interface for establishing TCP connections to a peer or peer group.
peer 5.5.5.5 as-number 100
peer 5.5.5.5 connect-interface loopback 0
address-family l2vpn evpn
Enter BGP EVPN address family view.
peer 4.4.4.4 enable
peer 4.4.4.4 enable
Enable BGP to exchange unicast routing information with a peer or peer group.
peer 5.5.5.5 enable
peer 5.5.5.5 enable
N/A
N/A
service-instance 1000
Create Ethernet service instance 1000.
encapsulation s-vid 2
Configure a frame match criterion for the Ethernet service instance.
xconnect vsi vpn1
xconnect vsi vpn1
Map VSI vpn1 to the Ethernet service instance.
service-instance 1001
Create Ethernet service instance 1001.
encapsulation s-vid 3
xconnect vsi vpn2
xconnect vsi vpn2
Map VSI vpn2 to the Ethernet service instance.
N/A
N/A
igmp-snooping
igmp-snooping
Enable IGMP snooping on the switch and enter IGMP-snooping view.
N/A
vsi vpn1
vsi vpn1
igmp-snooping enable
Enable IGMP snooping for the VSI.
pim-snooping enable
pim-snooping enable
Enable PIM snooping for the VSI.
igmp-snooping proxy enable
Enable IGMP snooping proxying for the VSI.
N/A
vsi vpn2
vsi vpn2
pim-snooping enable
pim-snooping enable
N/A
multicast-vpn vxlan vpn-instance vpn1 mode mdt
Create an MDT-based MVXLAN.
address-family ipv4
address-family ipv4
Enter MVXLAN IPv4 address family view.
source loopback 1 evpn-drni-group
Specify the virtual VTEP address of the DR member devices as the IP address of the source interface.
default-group 239.0.0.1
Configure the default group.
data-group 239.0.1.0 255.255.255.128
Configure the data group range.
Specify the IP addresses of the local and remote DR member devices.
N/A
N/A
multicast routing
multicast routing
Enable IP multicast routing for the public network.
N/A
multicast routing vpn-instance vpn1
Enable IP multicast routing for VPN instance vpn1.
N/A
pim
pim
Enable PIM for the public network.
c-bsr 1.1.1.1
c-bsr 2.2.2.2
Configure a candidate-BSR.
c-rp 1.1.1.1
c-rp 2.2.2.2
Configure a candidate-RP.
N/A
pim vpn-instance vpn1
Enable PIM for VPN instance vpn1.
c-bsr 1.2.3.4
c-bsr 1.2.3.4
c-rp 1.2.3.4
c-rp 1.2.3.4
Configure Switch E in the same way Switch A and Switch B are configured except that DRNI settings are not required on Switch E. For more information about interface and IP address assignment on Switch E, see Table 1. For more information about the configuration procedure, see "Configuring access devices Switch A and Switch B."
Switch E
address-family ipv4
source loopback 0
Specify Loopback 0 as the source interface.
N/A
N/A
multicast routing
N/A
N/A
pim
c-bsr 3.3.3.3
c-rp 3.3.3.3
N/A
c-bsr 3.3.3.3
c-rp 3.3.3.3
Configuring core devices
Switch C
Switch D
ip vpn-instance external_vpn
Create VPN instance external_vpn.
route-distinguisher 1:100
address-family ipv4
address-family ipv4
vpn-target 100:100 2:2
Configure route targets for the VPN instance.
N/A
N/A
address-family ipv4
address-family ipv4
vpn-target 2:2 1:2
vpn-target 2:2 1:2
address-family evpn
address-family evpn
vpn-target 1:1
vpn-target 1:1
N/A
N/A
ospf 1 router-id 4.4.4.4
ospf 1 router-id 5.5.5.5
Enable OSPF process 1 and specify a router ID for the process.
area 0.0.0.0
area 0.0.0.0
N/A
N/A
ospf 2 vpn-instance external_vpn
Enable OSPF process 2 and specify VPN instance external_vpn for the process.
area 0.0.0.0
area 0.0.0.0
N/A
N/A
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
Create Loopback 0 and enter loopback interface view.
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
Create Loopback 1 and enter loopback interface view.
pim sm
pim sm
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
N/A
Create Loopback 2 and enter loopback interface view.
pim sm
pim sm
N/A
l2vpn enable
l2vpn enable
Enable L2VPN.
Disable remote-MAC address learning.
Disable remote ARP learning for VXLANs.
evpn global-mac 0001-0002-0004
Configure the EVPN global MAC address.
vsi vpn1
vsi vpn1
vxlan 10
vxlan 10
Create VXLAN 10 and enter its view.
N/A
vpn-target auto
vpn-target auto
N/A
N/A
vsi vpn2
vsi vpn2
vxlan 20
vxlan 20
Create VXLAN 20 and enter its view.
N/A
vpn-target auto
vpn-target auto
N/A
N/A
Configure the MAC address of the VSI interface.
Enable local proxy ARP on the VSI interface.
pim distributed-dr
pim distributed-dr
igmp enable
igmp enable
Enable IGMP on the VSI interface.
pim sm
pim sm
Enable PIM SM on the VSI interface.
N/A
pim distributed-dr
pim distributed-dr
igmp enable
igmp enable
pim sm
pim sm
N/A
pim sm
pim sm
l3-vni 1000
l3-vni 1000
Configure the L3 VXLAN ID as 1000 for the VPN instance.
N/A
interface vsi-interface 4
Create VSI-interface 4.
ip binding vpn-instance external_vpn
Associate the VSI interface with VPN instance external_vpn.
pim sm
pim sm
l3-vni 2000
l3-vni 2000
Configure the L3 VXLAN ID as 2000 for the VPN instance.
N/A
vsi vpn1
vsi vpn1
N/A
vsi vpn2
vsi vpn2
N/A
evpn drni group 5.6.7.8
evpn drni local 4.4.4.4 remote 5.5.5.5
evpn drni local 5.5.5.5 remote 4.4.4.4
drni system-mac 0022-0022-0022
drni system-priority 22
drni keepalive ip destination 21.1.0.2 source 21.1.0.1
drni keepalive ip destination 21.1.0.1 source 21.1.0.2
N/A
interface hundredgige 1/0/32
N/A
Configure the aggregate interface as the IPP.
port trunk pvid vlan 4050
Configure the aggregate interface as a trunk port and set its PVID to 4050.
N/A
N/A
N/A
vlan 2 to 3 100
vlan 2 to 3 100
Create VLANs 2, 3, and 100.
N/A
port drni group 2
port drni group 2
xconnect vsi vpn1
xconnect vsi vpn1
Map the Ethernet service instance to VSI vpn1.
xconnect vsi vpn2
xconnect vsi vpn2
Map the Ethernet service instance to VSI vpn2.
N/A
N/A
interface bridge-aggregation 100
Create Layer 2 aggregate interface Bridge-Aggregation 100 and enter its view.
N/A
port link-aggregation group 100
Assign the interface to aggregation group 100.
N/A
Enter the view of Bridge-Aggregation 100.
port trunk permit vlan 100
Assign the aggregate interface to VLAN 100.
port drni group 100
port drni group 100
Assign the aggregate interface to DR group 100.
N/A
interface hundredgige 1/0/31
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
pim sm
pim sm
N/A
drni mad exclude interface hundredgige 1/0/28
drni mad exclude interface hundredgige 1/0/31
drink mad exclude interface loopback 0
drni mad exclude interface vlan-interface 100
drni mad exclude interface vsi-interface 4
bgp 100
bgp 100
router-id 4.4.4.4
router-id 5.5.5.5
group e internal
group e internal
Create a peer group.
peer e connect-interface loopback 0
peer 1.1.1.1 group e
Add peer 1.1.1.1 to the peer group.
peer 2.2.2.2 group e
Add peer 2.2.2.2 to the peer group.
peer 3.3.3.3 group e
Add peer 3.3.3.3 to the peer group.
undo policy vpn-target
Disable route target filtering for BGP EVPN routes.
peer e enable
peer e enable
peer e next-hop-local
Set the local router as the next hop for routes sent to a peer or peer group.
peer e reflect-client
Configure the local switch as a route reflector and specify peer group e as a client.
N/A
N/A
igmp-snooping
igmp-snooping
Enable IGMP snooping and enter IGMP-snooping view.
N/A
vlan 100
vlan 100
Create VLAN 100.
Enable IGMP snooping for the VLAN.
pim-snooping enable
pim-snooping enable
Enable PIM snooping for the VLAN.
igmp-snooping triggered-query enable port-down port-up
Enable the switch to send IGMP general queries when the state of a port changes.
N/A
Create VLAN-interface 100.
Associate the VLAN interface with VPN instance external_vpn.
pim sm
pim sm
Enable PIM SM.
pim distributed-dr
pim distributed-dr
Configure the VLAN interface as a distributed designated router interface.
pim triggered-hello enable port-down port-up
Enable the switch to send hello messages with a different Generation ID when the state of a port changes.
igmp enable
igmp enable
N/A
multicast-vpn vxlan vpn-instance external_vpn mode mdt
Create an MDT-based MVXLAN and enter MVXLAN view.
address-family ipv4
address-family ipv4
default-group 239.0.2.0
data-group 239.0.3.0 255.255.255.128
N/A
N/A
address-family ipv4
address-family ipv4
N/A
N/A
multicast routing
multicast routing
N/A
multicast routing vpn-instance external_vpn
Enable IP multicast routing for VPN instance external_vpn.
multicast extranet select-rpf l3-vni 1000 group 226.0.0.0 8
Configure an IPv4 MVXLAN extranet RPF selection policy.
N/A
N/A
pim
pim
c-bsr 4.4.4.4
c-bsr 5.5.5.5
c-rp 4.4.4.4
c-rp 5.5.5.5
N/A
pim vpn-instance external_vpn
Enable PIM for VPN instance external_vpn.
c-bsr 4.4.4.4
c-bsr 5.5.5.5
c-rp 4.4.4.4
c-rp 5.5.5.5
N/A
N/A
c-bsr 5.6.7.8
c-bsr 5.6.7.8
c-rp 5.6.7.8
c-rp 5.6.7.8
Overlay traffic forwarding models
Overlay traffic characteristics
The following table describes overlay traffic characteristics:
Parameter
No.
Overlay traffic number in the format of O-4-xxx or O-6-xxx.
O represents overlay, 4 represents IPv4, 6 represents IPv6, and xxx represents the traffic number starting from 001.
Traffic type
Traffic type, which is IPv4 multicast.
Direction
Traffic direction.
Traffic can be forwarded from leaf to border, east to north across leaf devices, and from border to leaf.
Forwarding path
List of nodes that the traffic passes through.
Traffic simulation
Simulation method used in the test. A tester is simulated as a server to transmit traffic.
Load
Traffic load is light or heavy.
If the number of flows is less than 1000, the load is light.
If the number of flows is more than 1000, the load is heavy.
Traffic direction to  firewalls/LB
Enter the method used to direct traffic to firewalls or LBs. In this example, no firewalls or LBs are deployed.
Forwarding models
No.
Traffic type
Direction
Forwarding path
Traffic simulation
Load
O-4-001
IPv4 multicast
East to west, across leaf devices
Server 1 > Switch A&Switch B > Switch E > Server 5
Bond4+ tester
Light
N/A
O-4-002
IPv4 multicast
Leaf to border
Server 1 > Switch A&Switch B > Switch C&Switch D > Server 4
Bond4+ tester
Light
N/A
Testing network convergence
Table 2 Network convergence
Device
Failure type
Traffic interruption time
Recovery type
Leaf
Single point of failure for ECMP uplinks
≤ 500 ms
Recovery from single point of failure for ECMP uplinks
0 ms
Single point of failure for DR member links
≤ 500 ms
Recovery from single point of failure for DR member links
≤ 150 ms
IPL failure
≤ 3000 ms
IPL failure recovery
≤ 4000 ms
Keepalive link failure
0 ms
Recovery from keepalive link failure
0 ms
Keepalive link and IPL failure
≤ 5000 ms
Recovery from keepalive link and IPL failure
≤ 8000 ms
Upgrading a device
≤ 3000 ms
Expanding the network
0 ms
Replacing hardware
≤ 3000 ms
Border
≤ 500 ms
0 ms
≤ 500 ms
≤ 150 ms
IPL failure
≤ 3000 ms
≤ 4000 ms
0 ms
0 ms
Second level for traffic forwarding recovery
Second level for traffic switchover
Upgrading a device
≤ 3000 ms
0 ms
Replacing hardware
≤ 3000 ms
Verification commands
Switch D
Switch E
display multicast-vpn vxlan { vpn-instance instance-name | public-instance } data-group receive [ brief | [ active | group group-address | sender source-address | vpn-source-address [ mask { mask-length | mask } ] | vpn-group-address [ mask { mask-length | mask } ] ] * ]
Displays received data group information in an MVXLAN.
display multicast-vpn vxlan { vpn-instance instance-name | public-instance } data-group send [ group group-address | vpn-source-address [ mask { mask-length | mask } ] | vpn-group-address [ mask { mask-length | mask } ] ] *
Displays sent data group information in an MVXLAN.
display multicast-vpn vxlan [ vpn-instance instance-name | public-instance ] default-group { local | remote }
Displays information about default groups.
The following information uses Switch A as an example.
# Display EVPN SMET routes.
<SwitchA> display bgp l2vpn evpn route-type smet
 Status codes: * - valid, > - best, d - dampened, h - history
               a - additional-path
 Total number of routes from all PEs: 3200
 Route distinguisher: 1:1(vpn1)
 Total number of routes: 2600
* >i [6][0][0][0.0.0.0][32][225.0.0.1][32][4.4.4.4]/128
                        4.4.4.4         0          100        0
     Path/Ogn: i
* >i [6][0][0][0.0.0.0][32][225.0.0.1][32][5.5.5.5]/128
                        5.5.5.5         0          100        0
     Path/Ogn: i
* >i [6][0][0][0.0.0.0][32][225.0.0.2][32][4.4.4.4]/128
                        4.4.4.4         0          100        0
     Path/Ogn: i
# Display S-PMSI routes.
<SwitchA> display bgp l2vpn evpn route-type s-pmsi
               a - additional-path
 Total number of routes from all PEs: 1010
 Total number of routes: 1507
* >  [10][0][0][0.0.0.0][0][0.0.0.0][32][1.1.1.1]/96
                        0.0.0.0         0          100        32768
     Path/Ogn: i
* >i [10][0][0][0.0.0.0][0][0.0.0.0][32][2.2.2.2]/96
                        2.2.2.2         0          100        0
     Path/Ogn: i
*  i                    2.2.2.2         0          100        0
     Path/Ogn: i
* >i [10][0][0][0.0.0.0][0][0.0.0.0][32][3.3.3.3]/96
                        3.3.3.3         0          100        0
     Path/Ogn: i
*  i                    3.3.3.3         0          100        0
     Path/Ogn: i
* >i [10][0][0][0.0.0.0][0][0.0.0.0][32][4.4.4.4]/96
                        4.4.4.4         0          100        0
     Path/Ogn: i
* >i [10][0][0][0.0.0.0][0][0.0.0.0][32][5.5.5.5]/96
                        5.5.5.5         0          100        0
# Display VXLAN tunnel information.
<SwitchA> display interface tunnel
Tunnel0
Current state: UP
Line protocol state: UP
Bandwidth: 64 kbps
Tunnel source 1.2.3.4, destination 4.4.4.4
Tunnel1
Current state: UP
Bandwidth: 64 kbps
Tunnel source 1.2.3.4, destination 5.6.7.8
Tunnel2
Current state: UP
Description: Tunnel2 Interface
Bandwidth: 64 kbps
Tunnel source 1.2.3.4, destination 5.5.5.5
Tunnel3
Current state: UP
Description: Tunnel3 Interface
Bandwidth: 64 kbps
Tunnel source 1.2.3.4, destination 3.3.3.3
# Display brief information about multicast tunnel interfaces.
<SwitchA> display interface mtunnel brief
Protocol: (s) - spoofing
Interface            Link Protocol Primary IP        Description
MTunnel0             UP   UP       1.2.3.4
MTunnel1             UP   UP       1.2.3.4
MTunnel2             UP   UP       1.2.3.4
MTunnel3             UP   UP       1.2.3.4
# Display PIM routing entries in VPN instance vpna.
<SwitchA> display pim vpn-instance vpna routing-table
 Total 1 (*, G) entries; 1 (S, G) entries
 (*, 225.0.0.0)
     RP: 12.12.12.12 (local)
     Protocol: pim-sm, Flag: WC RC
     UpTime: 03:01:20
     Upstream interface: Register-Tunnel0
         Upstream neighbor: NULL
         RPF prime neighbor: NULL
     Downstream interface information:
         1: MTunnel0
             Protocol: MD, UpTime: 02:57:31, Expires: -
2: Vsi-interface2
             Protocol: igmp, UpTime: 03:01:22, Expires: -
(10.1.1.10, 225.0.0.0)
     Protocol: pim-sm, Flag: SPT 2MSDP LOC ACT SQ RC 2MVPN
     UpTime: 03:01:20
     Upstream interface: Vsi-interface1
         1: MTunnel1
             Protocol: MD, UpTime: 02:56:31, Expires: -
2: Vsi-interface2
# Display the DR system settings.
[SwitchA] display drni system
IPP: BAGG1
State: UP
DR          System number System MAC         System priority
Local      1                0001-0001-0001    123
Peer       2                0001-0001-0001    123
# Display summary information about the IPP and DR interfaces.
[SwitchA] display drni summary
Global consistency check           : SUCCESS
Inconsistent type 1 global settings: -
IPP             IPP ID        State
BAGG1          1              UP
DR interface    DR group ID   State    Check result   Type 1 inconsistency
BAGG1            1               UP        SUCCESS         -
BAGG1            2               UP        SUCCESS         -
Upgrading the devices
Upgrading a leaf device
Checking the environment
Execute the commands in "Verification commands" and the following commands to verify that the device is available for an upgrade.
Leaf 1
Leaf 2
display device
display device
Displays device information.
display boot-loader
display boot-loader
Displays current software images and startup software images.
display version
display version
Displays system version information.
See H3C Switches DR System Upgrade & Replacement & Expansion Guide.
Verifying the traffic interruption time during the upgrade
Verify that the traffic interruption time is shorter than 500 ms during a switchover and shorter than 150 ms during fallback. For more information, see "Testing network convergence."
Verifying the upgrade result
Execute the commands in "Verification commands" and the following commands to verify that the device is upgraded successfully.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Upgrading a spine device
Spine 1
Spine 2
display device
display device
display boot-loader
display boot-loader
display version
display version
1.     Use the display version command to verify the current BootWare image version and startup software version.
2.     Use the release notes for the upgrade software version to evaluate the upgrade impact on your network and verify the following items:
¡     Software and hardware compatibility.
¡     Version and size of the upgrade software.
¡     Compatibility of the upgrade software with the current BootWare image and startup software image.
3.     Use the release notes to verify whether the software images require a license. If licenses are required, register and activate licenses for each license-based software image.
4.     Use the dir command to verify that the device has sufficient storage space for the upgrade images. If the storage space is not sufficient, delete unused files by using the delete command.
5.     Use FTP or TFTP to transfer the upgrade image file to the root directory of a file system.
6.     Upgrade the device according to the configuration guides for the device.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Upgrading a border device
Border 1
Border 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Border 1
Border 2
display device
display device
display boot-loader
display boot-loader
display version
display version
An expansion operation adds two leaf devices.
Adding a leaf device
Execute the commands in "Verification commands" and the following commands to verify that the device is available for an expansion.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Adding the device to the leaf tier
1.     Disconnect the device from network management systems.
2.     Upgrade the software of the device as needed.
3.     Preconfigure the device.
4.     Connect the device to network management systems.
5.     Incorporate the device on the controller.
Verifying the expansion result
Execute the following commands to verify that the device is added successfully.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Replacing hardware
Replacing a device
Execute the commands in "Verification commands" and the following commands to verify that the target device is available for a replacement.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Replacing the device
Verifying the replacement result
Execute the commands in "Checking the environment."