IPSG bindings synchronized by routing protocols
Configuring the IPv4SG feature
Configuring a static IPv4SG binding
Excluding IPv4 packets from IPSG filtering
Configuring the IPv6SG feature
Configuring a static IPv6SG binding
Setting the maximum number of IPv6SG bindings on an interface
Enabling SNMP notifications for IPSG
Display and maintenance commands for IPSG
Example: Configuring static IPv4SG
Example: Configuring DHCP snooping-based dynamic IPv4SG
Example: Configuring DHCP relay agent-based dynamic IPv4SG
Example: Configuring static IPv6SG
Example: Configuring DHCPv6 snooping-based dynamic IPv6SG address bindings
Example: Configuring DHCPv6 snooping-based dynamic IPv6SG prefix bindings
Example: Configuring DHCPv6 relay agent-based dynamic IPv6SG
Configuring IP source guard
About IPSG
IP source guard (IPSG) prevents spoofing attacks by using an IPSG binding table to filter out illegitimate packets. This feature is typically configured on user-side interfaces.
IPSG operating mechanism
The IPSG binding table contains bindings that bind IP address, MAC address, VLAN, or any combinations. IPSG uses the bindings to match an incoming packet. If a match is found, the packet is forwarded. If no match is found, the packet is discarded.
IPSG is a per-interface packet filter. Configuring this feature on one interface does not affect packet forwarding on another interface.
IPSG bindings can be static or dynamic.
As shown in Figure 1, IPSG forwards only the packets that match an IPSG binding.
Figure 1 IPSG application
Static IPSG bindings
Static IPSG bindings are configured manually. They are suitable for scenarios where few hosts exist on a LAN and their IP addresses are manually configured. For example, you can configure a static IPSG binding on an interface that connects to a server. This binding allows the interface to receive packets only from the server.
Static IPSG bindings on an interface implement the following functions:
· Filter incoming IPv4 or IPv6 packets on the interface.
· Cooperate with ARP attack detection in IPv4 for user validity checking. For information about ARP attack detection, see "Configuring ARP attack protection."
· Cooperate with ND attack detection in IPv6 for user validity checking. For information about ND attack detection, see "Configuring ND attack defense."
Static IPSG bindings can be global or interface-specific.
· Global static binding—Binds the IP address and MAC address in system view. The binding takes effect on all interfaces to filter packets for user spoofing attack prevention.
· Interface-specific static binding—Binds the IP address, MAC address, VLAN, or any combination of the items in interface view. The binding takes effect only on the interface to check the validity of users who are attempting to access the interface.
Dynamic IPSG bindings
IPSG automatically obtains user information from other modules to generate dynamic bindings. A dynamic IPSG binding can contain MAC address, IPv4 or IPv6 address, VLAN tag, ingress interface, and binding type. The binding type identifies the source module for the binding, such as DHCP snooping, DHCPv6 snooping, DHCP relay agent, or DHCPv6 relay agent.
For example, DHCP-based IPSG bindings are suitable for scenarios where hosts on a LAN obtain IP addresses through DHCP. IPSG is configured on the DHCP server, the DHCP snooping device, or the DHCP relay agent. It generates dynamic bindings based on the client bindings on the DHCP server, the DHCP snooping entries, or the DHCP relay entries. IPSG allows only packets from the DHCP clients to pass through.
Dynamic IPv4SG
Dynamic bindings generated based on different source modules are for different usages:
Interface types |
Source modules |
Binding usage |
Layer 2 Ethernet interface |
DHCP snooping 802.1X |
Packet filtering. |
ARP snooping |
For cooperation with modules (such as the MFF module) to provide security services. |
VLAN interface |
DHCP relay agent |
Packet filtering. |
DHCP server |
For cooperation with modules (such as the authorized ARP module) to provide security services. |
For more information about 802.1X, see "Configuring 802.1X." For information about ARP snooping, DHCP snooping, DHCP relay, and DHCP server, see Layer 3—IP Services Configuration Guide.
Dynamic IPv6SG
Dynamic IPv6SG bindings generated based on different source modules are for different usages:
Interface types |
Source modules |
Binding usage |
DHCPv6 snooping ND snooping 802.1X |
Packet filtering. |
VLAN interface |
DHCPv6 relay agent ND RA prefix entry recording |
Packet filtering. |
DHCPv6 server |
Reporting bindings to the controller to provide online and offline user information. |
For more information about DHCPv6 snooping, see Layer 3—IP Services Configuration Guide. For more information about ND snooping, see IPv6 basics configuration in Layer 3—IP Services Configuration Guide. For more information about ND RA prefix entry recording, see IPv6 neighbor discovery in Layer 3—IP Services Configuration Guide. For more information about DHCPv6 relay agent, see Layer 3—IP Services Configuration Guide. For more information about DHCPv6 server, see Layer 3—IP Services Configuration Guide.
In addition to static and dynamic IPSG bindings, the device also supports IPSG bindings synchronized by routing protocols from remote devices. These bindings are called remote IPSG bindings. By default, the remote IPSG bindings do not have interface information and cannot be used for packet filtering. When users roam from remote devices to the local device, the device learns interface information for the remote IPSG bindings through ARP or ND entries of the users. Then, the device converts the remote IPSG bindings into local IPSG bindings and uses these bindings for packet filtering.
IPSG tasks at a glance
To configure IPSG, perform the following tasks:
1. To configure IPv4SG, perform the following tasks:
b. (Optional.) Configuring a static IPv4SG binding
c. (Optional.) Excluding IPv4 packets from IPSG filtering
2. To configure IPv6SG, perform the following tasks:
b. (Optional.) Configuring a static IPv6SG binding
c. (Optional.) Setting the maximum number of IPv6SG bindings on an interface
3. Enabling SNMP notifications for IPSG
Enabling IPv4SG
When you enable IPSG on an interface, the static and dynamic IPSG are both enabled.
· Static IPv4SG uses static bindings configured by using the ip source binding command. For more information, see "Configuring a static IPv4SG binding."
· Dynamic IPv4SG generates dynamic bindings from related source modules. IPv4SG uses the bindings to filter incoming IPv4 packets based on the matching criteria specified in the ip verify source command.
To implement dynamic IPv4SG, make sure 802.1X, ARP snooping, DHCP snooping, DHCP relay agent, or DHCP server operates correctly on the network.
You can enable IPv4SG on an interface or in a VLAN. The interface-specific configuration applies to this interface. The VLAN-specific configuration applies to all Layer 2 Ethernet interfaces that belong to this VLAN.
Do not configure IPv4SG both in a VLAN and on an Ethernet interface that belongs to the VLAN. Before you perform one of the configurations, make sure the other configuration does not exist.
Enabling IPv4SG on an interface
1. Enter system view.
2. Enter interface view.
The following interface types are supported:
¡ Layer 2 Ethernet interface.
¡ VLAN interface.
3. Enable the IPv4SG feature.
By default, the IPv4SG feature is disabled on an interface.
Enabling IPv4SG in a VLAN
2. Enter VLAN view.
vlan vlan-id
3. Enable IPv4SG in the VLAN.
By default, IPv4SG is disabled in a VLAN.
You can configure global static and interface-specific static IPv4SG bindings. Interface-specific static and dynamic bindings take priority over global static bindings. An interface first uses the static and dynamic bindings on the interface to match packets. If no match is found, the interface uses the global bindings.
Global static bindings take effect on all interfaces on the device.
To configure a static IPv4SG binding for the ARP attack detection feature, make sure the following conditions are met:
· The ip-address ip-address option, the mac-address mac-address option, and the vlan vlan-id option must be specified.
· ARP attack detection must be enabled for the specified VLAN.
Configuring a global static IPv4SG binding
2. Configure a global static IPv4SG binding.
Configuring a static IPv4SG binding on an interface
¡ VLAN interface.
3. Configure a static IPv4SG binding.
ip source binding { ip-address ip-address | ip-address ip-address mac-address mac-address | mac-address mac-address } [ vlan vlan-id ]
You can configure the same static IPv4SG binding on different interfaces.
By default, IPv4SG processes all incoming IPv4 packets on an interface and discards the packets that do not match IPSG bindings. To allow specific IPv4 packets that do not match any IPSG binding to pass through the interface, you can specify source items of the packets for IPSG filtering exemption. All IPv4 packets with the specified source items are forwarded without being processed by IPSG.
2. Exclude IPv4 packets with the specified source items from IPSG filtering.
ip verify source exclude vlan start-vlan-id [ to end-vlan-id ]
By default, no excluded source items are configured.
You can execute this command multiple times to specify multiple excluded VLANs. The specified excluded VLANs cannot overlap.
Enabling IPv6SG
When you enable IPv6SG on an interface, the static and dynamic IPv6SG are both enabled.
· Static IPv6SG uses static bindings configured by using the ipv6 source binding command. For more information, see "Configuring a static IPv6SG binding."
· Dynamic IPv6SG generates dynamic bindings from related source modules. IPv6SG uses the bindings to filter incoming IPv6 packets based on the matching criteria specified in the ipv6 verify source command.
In a VLAN enabled with IPv6SG, you can configure an interface as an IPv6SG trusted port if you can determine that no attack sources are connect to the interface. IPv6SG does not filter incoming packets on that trusted interface.
To implement dynamic IPv6SG, make sure DHCPv6 snooping, DHCPv6 relay agent, or ND snooping operates correctly on the network.
You can enable IPv6SG on an interface or in a VLAN. The interface-specific configuration applies to this interface. The VLAN-specific configuration applies to all Layer 2 Ethernet interfaces that belong to this VLAN.
Do not configure IPv6SG both in a VLAN and on an Ethernet interface that belongs to the VLAN. Before you perform one of the configurations, make sure the other configuration does not exist.
Enabling IPv6SG on an interface
¡ VLAN interface.
3. Enable the IPv6SG feature.
By default, the IPv6SG feature is disabled on an interface.
Enabling IPv6SG in a VLAN
2. Enter VLAN view.
vlan vlan-id
3. Enable IPv6SG in the VLAN.
By default, IPv6SG is disabled in a VLAN.
You can configure global static and interface-specific static IPv6SG bindings. Interface-specific static and dynamic bindings take priority over global static bindings. An interface first uses the static and dynamic bindings on the interface to match packets. If no match is found, the interface uses the global bindings.
To configure a static IPv6SG binding for the ND attack detection feature, the vlan vlan-id option must be specified, and ND attack detection must be enabled for the specified VLAN.
Configuring a global static IPv6SG binding
2. Configure a global static IPv6SG binding.
Configuring a static IPv6SG binding on an interface
¡ VLAN interface.
3. Configure a static IPv6SG binding.
ipv6 source binding { ip-address ipv6-address | ip-address ipv6-address mac-address mac-address | mac-address mac-address } [ vlan vlan-id ]
You can configure the same static IPv6SG binding on different interfaces.
You can set the maximum number of IPv6SG bindings on an interface to limit the total number of static and dynamic IPv6SG bindings on the interface. If the upper limit is reached, no more IPv6SG bindings can be added on the interface.
2. Enter Layer 2 Ethernet interface view.
3. Set the maximum number of IPv6SG bindings on the interface.
ipv6 verify source max-entries number
By default, the maximum number of IPv6SG bindings is not limited on an interface.
To report critical IPSG events to an NMS, enable SNMP notifications for IPSG. For example, If you enable the device to generate notifications when the number of packets dropped by IPSG per second on an interface has reached, exceeded, or dropped below the alarm threshold, the device works as follows:
· When the number of packets dropped by IPSG per second on an interface is equal to or greater than the IPv4SG or IPv6SG alarm threshold, the device sends a notification.
· When the number of packets dropped by IPSG per second on an interface drops below the IPv4SG or IPv6SG alarm threshold, the device reports a threshold recovery event.
To set the IPv4 or IPv6SG alarm threshold, execute the ip verify source alarm or ipv6 verify source alarm command, respectively.
For SNMP notifications to be sent correctly, you must also configure SNMP on the device. For more information about SNMP and information center configuration, see Network Management and Monitoring Guide.
2. Enable SNMP notifications for IPSG.
snmp-agent trap enable ipsg [ drop-threshold ]
By default, SNMP notifications for IPSG are enabled.
Task |
Command |
Display IPv4SG bindings. |
display ip source binding [ static | [ vpn-instance vpn-instance-name ] [ arp-snooping-vlan | dhcp-relay | dhcp-server | dhcp-snooping | dot1x | remote ] ] [ ip-address ip-address ] [ mac-address mac-address ] [ vlan vlan-id ] [ interface interface-type interface-number ] [ slot slot-number ] |
Display local IPv4SG bindings that can be synchronized by routing protocols. |
display ip source binding-local [ interface interface-type interface-number ] [ dhcp-relay ] [ ip-address ip-address ] [ mac-address mac-address ] [ vlan vlan-id ] [ slot slot-number ] |
Display remote IPv4SG bindings synchronized by routing protocols. |
display ip source binding-remote [ router-id router-id ] [ dhcp-relay ] [ ip-address ip-address ] [ mac-address mac-address ] [ vlan vlan-id ] [ slot slot-number ] |
Display statistics about local and remote IPv4SG bindings that routing protocols synchronize. |
display ip source binding statistics |
Display source items that have been configured to be excluded from IPSG filtering. |
display ip verify source excluded [ vlan start-vlan-id [ to end-vlan-id ] ] [ slot slot-number ] |
Display IPv6SG address bindings. |
display ipv6 source binding [ static | [ vpn-instance vpn-instance-name ] [ dhcpv6-relay | dhcpv6-server | dhcpv6-snooping | dot1x | nd-snooping-vlan | remote ] ] [ ip-address ipv6-address ] [ mac-address mac-address ] [ vlan vlan-id ] [ interface interface-type interface-number ] [ slot slot-number ] |
Display local IPv6SG bindings that can be synchronized by routing protocols. |
display ipv6 source binding-local [ interface interface-type interface-number ] [ dhcpv6-relay | nd-snooping-vlan ] [ ip-address ipv6-address ] [ mac-address mac-address ] [ vlan vlan-id ] [ slot slot-number ] |
Display remote IPv6SG bindings synchronized by routing protocols. |
display ipv6 source binding-remote [ router-id router-id ] [ dhcpv6-relay | nd-snooping-vlan] [ ip-address ipv6-address ] [ mac-address mac-address ] [ vlan vlan-id ] [ slot slot-number ] |
Display IPv6SG prefix bindings. |
display ipv6 source binding pd [ vpn-instance vpn-instance-name ] [ prefix prefix/prefix-length ] [ mac-address mac-address ] [ vlan vlan-id ] [ interface interface-type interface-number ] [ slot slot-number ] |
Display statistics about local and remote IPv6SG bindings that routing protocols synchronize. |
display ipv6 source binding statistics |
IPSG configuration examples
As shown in Figure 2, all hosts use static IP addresses.
Configure static IPv4SG bindings on Device A and Device B to meet the following requirements:
· All interfaces of Device A allow IP packets from Host A to pass.
· GigabitEthernet 1/0/1 of Device A allows IP packets from Host B to pass.
# Configure IP addresses for the interfaces. (Details not shown.)
# Enable IPv4SG on GigabitEthernet 1/0/2.
[DeviceA-GigabitEthernet1/0/2] ip verify source ip-address mac-address
# Configure a static IPv4SG binding for Host A.
[DeviceA] ip source binding ip-address 192.168.0.1 mac-address 0001-0203-0406
# Enable IPv4SG on GigabitEthernet 1/0/1.
[DeviceA-GigabitEthernet1/0/1] ip verify source ip-address mac-address
# On GigabitEthernet 1/0/1, configure a static IPv4SG binding for Host B.
[DeviceA-GigabitEthernet1/0/1] ip source binding mac-address 0001-0203-0407
# Verify that the static IPv4SG bindings are configured successfully on Device A.
<DeviceA> display ip source binding static
Total entries found: 2
IP address MAC address Interface VLAN Type
192.168.0.1 0001-0203-0406 N/A N/A Static
N/A 0001-0203-0407 GE1/0/1 N/A Static
As shown in Figure 3, the host (the DHCP client) obtains an IP address from the DHCP server. Perform the following tasks:
· Enable DHCP snooping on the device to make sure the DHCP client obtains an IP address from the authorized DHCP server. To generate a DHCP snooping entry for the DHCP client, enable recording of client information in DHCP snooping entries.
· Enable dynamic IPv4SG on GigabitEthernet 1/0/1 to filter incoming packets by using the IPv4SG bindings generated based on DHCP snooping entries. Only packets from the DHCP client are allowed to pass.
1. Configure the DHCP server.
For information about DHCP server configuration, see Layer 3—IP Services Configuration Guide.
2. Configure the device:
# Enable DHCP snooping.
[Device] dhcp snooping enable
# Configure GigabitEthernet 1/0/2 as a trusted interface.
[Device-GigabitEthernet1/0/2] dhcp snooping trust
# Enable IPv4SG on GigabitEthernet 1/0/1 and verify the source IP address and MAC address for dynamic IPSG.
[Device-GigabitEthernet1/0/1] ip verify source ip-address mac-address
# Enable recording of client information in DHCP snooping entries on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] dhcp snooping binding record
# Display dynamic IPv4SG bindings generated based on DHCP snooping entries.
[Device] display ip source binding dhcp-snooping
Total entries found: 1
192.168.0.1 0001-0203-0406 GE1/0/1 1 DHCP snooping
GigabitEthernet 1/0/1 will filter packets based on the IPv4SG binding.
As shown in Figure 4, DHCP relay agent is enabled on the switch. The host obtains an IP address from the DHCP server through the DHCP relay agent.
Enable dynamic IPv4SG on VLAN-interface 100 to filter incoming packets by using the IPv4SG bindings generated based on DHCP relay entries.
1. Configure dynamic IPv4SG:
# Enable IPv4SG on VLAN-interface 100 and verify the source IP address and MAC address for dynamic IPSG.
<Switch> system-view
[Switch-Vlan-interface100] ip verify source ip-address mac-address
2. Configure the DHCP relay agent:
# Enable the DHCP service.
[Switch] dhcp enable
# Enable recording DHCP relay entries.
[Switch] dhcp relay client-information record
# Configure VLAN-interface 100 to operate in DHCP relay mode.
[Switch-Vlan-interface100] dhcp select relay
# Specify the IP address of the DHCP server.
[Switch-Vlan-interface100] dhcp relay server-address 10.1.1.1
# Display dynamic IPv4SG bindings generated based on DHCP relay entries.
[Switch] display ip source binding dhcp-relay
192.168.0.1 0001-0203-0406 Vlan100 100 DHCP relay
VLAN-interface 100 will filter packets based on the IPv4SG binding.
As shown in Figure 5, configure a static IPv6SG binding on GigabitEthernet 1/0/1 of the device to allow only IPv6 packets from the host to pass.
# Enable IPv6SG on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] ipv6 verify source ip-address mac-address
# On GigabitEthernet 1/0/1, configure a static IPv6SG binding for the host.
[Device-GigabitEthernet1/0/1] ipv6 source binding ip-address 2001::1 mac-address 0001-0202-0202
# Verify that the static IPv6SG binding is configured successfully on the device.
[Device] display ipv6 source binding static
IPv6 address MAC address Interface VLAN Type
2001::1 0001-0202-0202 GE1/0/1 N/A Static
As shown in Figure 6, the host (the DHCPv6 client) obtains an IP address from the DHCPv6 server. Perform the following tasks:
· Enable DHCPv6 snooping on the device to make sure the DHCPv6 client obtains an IPv6 address from the authorized DHCPv6 server. To generate a DHCPv6 snooping entry for the DHCPv6 client, enable recording of client information in DHCPv6 snooping entries.
· Enable dynamic IPv6SG on GigabitEthernet 1/0/1 to filter incoming packets by using the IPv6SG bindings generated based on DHCPv6 snooping entries. Only packets from the DHCPv6 client are allowed to pass.
1. Configure DHCPv6 snooping:
# Enable DHCPv6 snooping globally.
[Device] ipv6 dhcp snooping enable
[Device-GigabitEthernet1/0/2] ipv6 dhcp snooping trust
2. Enable IPv6SG:
# Enable IPv6SG on GigabitEthernet 1/0/1 and verify the source IP address and MAC address for dynamic IPv6SG.
# Enable recording of client information in DHCPv6 snooping entries on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] ipv6 dhcp snooping binding record
# Display dynamic IPv6SG bindings generated based on DHCPv6 snooping entries.
[Device] display ipv6 source binding dhcpv6-snooping
2001::1 040a-0000-0001 GE1/0/1 1 DHCPv6 snooping
GigabitEthernet 1/0/1 will filter packets based on the IPv6SG binding.
As shown in Figure 7, the host (the DHCPv6 client) obtains an IPv6 prefix from the DHCPv6 server. Perform the following tasks:
· Enable DHCPv6 snooping on the device to make sure the DHCPv6 client obtains an IPv6 prefix from the authorized DHCPv6 server. To generate a DHCPv6 snooping prefix entry for the DHCPv6 client, enable recording IPv6 prefix information in DHCPv6 snooping entries.
· Enable dynamic IPv6SG on GigabitEthernet 1/0/1 to filter incoming packets by using the IPv6SG bindings generated based on DHCPv6 snooping prefix entries. Only packets from the DHCPv6 client are allowed to pass.
1. Configure DHCPv6 snooping.
# Enable recording DHCPv6 snooping prefix entries on GigabitEthernet 1/0/1.
[Device-GigabitEthernet1/0/1] ipv6 dhcp snooping pd binding record
2. Enable IPv6SG.
[Device] display ipv6 source binding pd
2001:410:1::/48 0010-9400-0004 GE1/0/1 1
As shown in Figure 8, DHCPv6 relay agent is enabled on the switch. The clients obtain IPv6 addresses from the DHCPv6 server through the DHCPv6 relay agent.
Enable dynamic IPv6SG on VLAN-interface 3 to filter incoming packets by using the IPv6SG bindings generated based on DHCPv6 relay entries.
1. Configure the DHCPv6 relay agent:
# Create VLAN 2 and VLAN 3, assign interfaces to the VLANs, and specify IP addresses for VLAN-interface 2 and VLAN-interface 3. (Details not shown.)
# Enable the DHCPv6 relay agent on VLAN-interface 3.
[Switch-Vlan-interface3] ipv6 dhcp select relay
# Enable recording of DHCPv6 relay entries on the interface.
[Switch-Vlan-interface3] ipv6 dhcp relay client-information record
# Specify the DHCPv6 server address 2::2 on the relay agent.
[Switch-Vlan-interface3] ipv6 dhcp relay server-address 2::2
2. Enable IPv6SG on VLAN-interface 3 and verify the source IP address and MAC address for dynamic IPv6SG.
[Switch-Vlan-interface3] ipv6 verify source ip-address mac-address
[Switch-Vlan-interface3] quit
# Display dynamic IPv6SG bindings generated based on DHCPv6 relay entries.
[Switch] display ipv6 source binding dhcpv6-relay
IP Address MAC Address Interface VLAN Type
1::2 0001-0203-0406 Vlan3 3 DHCPv6 relay
VLAN-interface 3 will filter packets based on the IPv6SG binding.