- 11-High Availability Configuration Guide
- 01-Ethernet OAM configuration
- 02-DLDP configuration
- 03-RRPP configuration
- 04-ERPS configuration
- 05-Smart Link configuration
- 06-Monitor Link configuration
- 07-Error code detection configuration
- 08-VRRP configuration
- 09-VSRP configuration
- 10-BFD configuration
- 11-Track configuration
- 12-Process placement configuration
- 13-Interface collaboration configuration
- 14-Reth interface and redundancy group configuration
| 03-RRPP configuration | 506.60 KB |
Restrictions and guidelines: RRPP configuration
Restrictions and guidelines for RRPP timer configuration
Configuring the Hello timer and Fail timer
Configuring the link-up delay timer
Configuring an RRPP ring group
Enabling SNMP notifications for RRPP
Display and maintenance commands for RRPP
Example: Configuring a single ring
Example: Configuring intersecting rings
Example: Configuring load-balanced intersecting rings
The primary node cannot receive Hello packets when the link state is normal
Configuring RRPP
About RRPP
The Rapid Ring Protection Protocol (RRPP) is an H3C-proprietary link layer protocol designed for Ethernet rings. RRPP can prevent broadcast storms caused by data loops when an Ethernet ring is healthy. RRPP can also rapidly restore the communication paths between the nodes when a link is disconnected on the ring. Compared with the spanning tree protocol, the convergence time of RRPP is fast and independent of the number of nodes in the Ethernet ring. RRPP is applicable to large-diameter networks.
RRPP networking
Figure 1 shows a typical RRPP network with two Ethernet rings and multiple nodes. RRPP detects ring status and sends topology change information by exchanging Rapid Ring Protection Protocol Data Units (RRPPDUs) among the nodes.
Figure 1 RRPP networking diagram
RRPP domain
An RRPP domain is uniquely identified by a domain ID. The interconnected devices with the same domain ID and control VLANs constitute an RRPP domain. An RRPP domain contains the following elements:
· Primary ring and subring.
· Control VLAN.
· Master node, transit node, edge node, and assistant edge node.
· Primary port, secondary port, common port, and edge port.
As shown in Figure 1, Domain 1 is an RRPP domain, containing two RRPP rings: Ring 1 and Ring 2. All the nodes on the two RRPP rings belong to the RRPP domain.
RRPP ring
A ring-shaped Ethernet topology is called an RRPP ring. RRPP rings include primary rings and subrings. You can configure a ring as either the primary ring or a subring by specifying its ring level. The primary ring is of level 0, and a subring is of level 1. An RRPP domain contains one or multiple RRPP rings, one serving as the primary ring and the others serving as subrings. A ring can be in one of the following states:
· Health state—All physical links on the Ethernet ring are connected.
· Disconnect state—Some physical links on the Ethernet ring are not connected.
As shown in Figure 1, Domain 1 contains two RRPP rings: Ring 1 and Ring 2. The level is set to 0 for Ring 1 and 1 for Ring 2. Ring 1 is configured as the primary ring, and Ring 2 is configured as a subring.
Control VLAN and protected VLAN
1. Control VLAN
In an RRPP domain, a control VLAN is dedicated to transferring RRPPDUs. On a device, the ports accessing an RRPP ring belong to the control VLANs of the ring, and only these ports can join the control VLANs.
An RRPP domain is configured with the following control VLANs:
¡ One primary control VLAN, which is the control VLAN for the primary ring.
¡ One secondary control VLAN, which is the control VLAN for subrings.
After you specify a VLAN as the primary control VLAN, the system automatically configures the secondary control VLAN. The VLAN ID is the primary control VLAN ID plus one. All subrings in the same RRPP domain share the same secondary control VLAN. IP address configuration is prohibited on the control VLAN interfaces.
2. Protected VLAN
A protected VLAN is dedicated to transferring data packets. Both RRPP ports and non-RRPP ports can be assigned to a protected VLAN.
Node role
Each device on an RRPP ring is a node. The role of a node is configurable. RRPP has the following node roles:
· Master node—Each ring has only one master node. The master node initiates the polling mechanism and determines the operations to be performed after a topology change.
· Transit node—On the primary ring, transit nodes refer to all nodes except the master node. On the subring, transit nodes refer to all nodes except the master node and the nodes where the primary ring intersects with the subring. A transit node monitors the state of its directly connected RRPP links and notifies the master node of the link state changes, if any. Based on the link state changes, the master node determines the operations to be performed.
· Edge node—A special node residing on both the primary ring and a subring at the same time. An edge node acts as a master node or transit node on the primary ring and as an edge node on the subring.
· Assistant edge node—A special node residing on both the primary ring and a subring at the same time. An assistant edge node acts as a master node or transit node on the primary ring and as an assistant edge node on the subring. This node works in conjunction with the edge node to detect the integrity of the primary ring and to perform loop guard.
As shown in Figure 1, Ring 1 is the primary ring and Ring 2 is a subring. Device A is the master node of Ring 1. Device B, Device C, and Device D are the transit nodes of Ring 1. Device E is the master node of Ring 2, Device B is the edge node of Ring 2, and Device C is the assistant edge node of Ring 2.
Port role
1. Primary port and secondary port
Each master node or transit node has two ports connected to an RRPP ring, a primary port and a secondary port. You can determine the role of a port.
In terms of functionality, the primary port and the secondary port of a master node have the following differences:
¡ The primary port and the secondary port are designed to play the role of sending and receiving Hello packets, respectively.
¡ When an RRPP ring is in Health state, the secondary port logically denies protected VLANs and permits only the packets from the control VLANs.
¡ When an RRPP ring is in Disconnect state, the secondary port forwards packets from protected VLANs.
In terms of functionality, the primary port and the secondary port of a transit node are the same. Both are designed for transferring protocol packets and data packets over an RRPP ring.
As shown in Figure 1, Device A is the master node of Ring 1. Port 1 and Port 2 are the primary port and the secondary port of the master node on Ring 1, respectively. Device B, Device C, and Device D are the transit nodes of Ring 1. Their Port 1 and Port 2 are the primary port and the secondary port on Ring 1, respectively.
2. Common port and edge port
The ports connecting the edge node and assistant edge node to the primary ring are common ports. The ports connecting the edge node and assistant edge node only to the subrings are edge ports. You can determine the role of a port.
As shown in Figure 1, Device B and Device C reside on Ring 1 and Ring 2. Device B's Port 1 and Port 2 and Device C's Port 1 and Port 2 access the primary ring, so they are common ports. Device B's Port 3 and Device C's Port 3 access only the subring, so they are edge ports.
RRPP ring group
To reduce Edge-Hello traffic, you can configure a group of subrings on the edge node or assistant edge node. You must configure a device as the edge node of these subrings, and another device as the assistant edge node of these subrings. Additionally, the subrings of the edge node and assistant edge node must connect to the same subring packet tunnels in major ring (SRPTs). Edge-Hello packets of the edge node of these subrings travel to the assistant edge node of these subrings over the same link.
An RRPP ring group configured on the edge node is an edge node RRPP ring group. An RRPP ring group configured on an assistant edge node is an assistant edge node RRPP ring group. Only one subring in an edge node RRPP ring group is allowed to send Edge-Hello packets.
RRPPDUs
Table 1 RRPPDU types and their functions
Type |
Hello |
The master node sends Hello packets (also known as Health packets) to detect the integrity of a ring in a network. |
Link-Down |
When a port on the transit node, edge node, or assistant edge node fails, the node initiates Link-Down packets to notify the master node of the disconnection of the ring. |
Common-Flush-FDB |
When an RRPP ring transits to Disconnect state, the master node initiates Common-Flush-FDB (FDB stands for Forwarding Database) packets. It uses the packets to instruct the transit nodes, edge nodes, and assistant edge nodes to update their own MAC address entries and ARP/ND entries. |
Complete-Flush-FDB |
When an RRPP ring transits to Health state, the master node sends Complete-Flush-FDB packets for the following purposes: · Instruct the transit nodes, edge nodes, and assistant edge nodes to update their MAC address entries and ARP/ND entries. · Instruct the transit nodes to unblock temporarily blocked ports. |
Edge-Hello |
The edge node sends Edge-Hello packets to examine the SRPTs between the edge node and the assistant edge node. |
Major-Fault |
The assistant edge node sends Major-Fault packets to notify the edge node of SRPT failure when an SRPT between assistant edge node and edge node is disconnected. |
RRPP timers
When RRPP determines the link state of an Ethernet ring, it uses the following timers:
Hello timer
The Hello timer specifies the interval at which the master node sends Hello packets out of the primary port.
Fail timer
The Fail timer specifies the maximum delay of Hello packets sent from the primary port to the secondary port of the master node. If the secondary port receives the Hello packets sent by the local master node before the Fail timer expires, the ring is in Health state. If the secondary port does not receive the Hello packets before the Fail timer expires, the ring transits to Disconnect state.
In an RRPP domain, a transit node learns the Fail timer value on the master node through the received Hello packets. This ensures that all nodes in the ring network have consistent Fail timer settings.
Link-up delay timer
This feature prevents frequent switchover of RRPP traffic forwarding paths caused by unstable RRPP port states. This feature behaves differently depending on whether you specify the distribute keyword in the linkup-delay-timer command.
· If you do not specify the distribute keyword, the master node starts the link-up delay timer when a faulty port comes up and the master node receives Hello packets from the secondary port.
¡ If the master node can still receive Hello packets from the secondary port after the link-up delay timer expires, the master node performs the following operations:
- Changes the RRPP ring state from Disconnect to Health.
- Switches the traffic from the secondary port to the primary port.
¡ If the master node cannot receive Hello packets from the secondary port after the Fail timer expires and before the link-up delay timer expires, the master node performs the following operations:
- Stops the link-up delay timer.
- Keeps the RRPP ring in Disconnect state.
· If you specify the distribute keyword, all nodes in the RRPP domain can learn the value of the link-up delay timer through Hello packets. When the faulty port comes up, the master node performs the following operations:
¡ The hosting RRPP node blocks the faulty port (the faulty port cannot send or receive any packets).
¡ Starts the link-up delay timer.
If the port does not become faulty after the link-up delay timer expires, the hosting RRPP node sets the port state to up. The master node can receive Hello packets from its secondary port again. Then, the master node changes the RRPP ring state from Disconnect to Health and switches the traffic from the secondary port to the primary port.
If the port becomes faulty again before the link-up delay timer expires, the hosting RRPP node blocks the port and stops the link-up delay timer.
How RRPP works
Polling mechanism
The polling mechanism is used by the master node of an RRPP ring to examine the Health state of the ring network.
The master node sends Hello packets out of its primary port at the Hello interval. These Hello packets travel through each transit node on the ring in turn.
· If the ring is complete, the secondary port of the master node receives Hello packets before the Fail timer expires. The master node keeps the secondary port blocked.
· If the ring is disconnected, the secondary port of the master node fails to receive Hello packets before the Fail timer expires. The master node releases the secondary port from blocking protected VLANs. It sends Common-Flush-FDB packets to instruct all transit nodes to update their own MAC address entries and ARP/ND entries.
Load balancing
In a ring network, traffic from multiple VLANs might be transmitted at the same time. RRPP can implement load balancing by transmitting traffic from different VLANs along different paths.
You can configure multiple RRPP domains for a ring network. Each RRPP domain transmits the traffic from the specified VLANs (protected VLANs). Traffic from different VLANs can be transmitted according to different topologies in the ring network for load balancing.
As shown in Figure 6, Ring 1 is configured as the primary ring of Domain 1 and Domain 2, which are configured with different protected VLANs. Device A is the master node of Ring 1 in Domain 1. Device B is the master node of Ring 1 in Domain 2. With such configurations, traffic from different VLANs can be transmitted on different links for load balancing in the single-ring network.
Link down alarm mechanism
In an RRPP domain, when the transit node, edge node, or assistant edge node finds that any of its ports is down, it immediately sends Link-Down packets to the master node. When the master node receives a Link-Down packet, it takes the following actions:
· Releases the secondary port from blocking protected VLANs.
· Sends Common-Flush-FDB packets to instruct all the transit nodes, edge nodes, and assistant edge nodes to update their MAC address entries and ARP/ND entries.
After each node updates its own entries, traffic is switched to the normal link.
Ring recovery
When the ports in an RRPP domain on the transit nodes, edge nodes, or assistant edge nodes come up again, the ring is recovered. However, the master node might detect the ring recovery after a period of time. A temporary loop might arise in the protected VLAN during this period. As a result, a broadcast storm occurs.
To prevent such cases, non-master nodes block the ports immediately when they find the ports accessing the ring are brought up again. The nodes block only the packets from the protected VLAN, and they permit only the packets from the control VLAN to pass through. The blocked ports are activated only when the nodes determine that no loop will be generated by these ports.
Broadcast storm suppression mechanism in case of SRPT failure in a multi-homed subring
As shown in Figure 5, Ring 1 is the primary ring, and Ring 2 and Ring 3 are subrings. When the two SRPTs between the edge node and the assistant edge node are down, the master nodes of Ring 2 and Ring 3 will open their secondary ports. A loop is generated among Device B, Device C, Device E, and Device F, causing a broadcast storm.
To avoid generating a loop, the edge node will temporarily block the edge port. The blocked edge port is activated only when the edge node determines that no loop will be generated when the edge port is activated.
RRPP ring group
In an edge node RRPP ring group, only the activated subring with the smallest domain ID and ring ID can send Edge-Hello packets. In an assistant edge node RRPP ring group, any activated subring that has received Edge-Hello packets will forward these packets to the other activated subrings. When an edge node RRPP ring group and an assistant edge node RRPP ring group are configured, the CPU workload is reduced because of the following reasons:
· Only one subring sends Edge-Hello packets on the edge node.
· Only one subring receives Edge-Hello packets on the assistant edge node.
As shown in Figure 5, Device B is the edge node of Ring 2 and Ring 3. Device C is the assistant edge node of Ring 2 and Ring 3. Device B and Device C need to send or receive Edge-Hello packets frequently. If more subrings are configured or more domains are configured for load balancing, Device B and Device C will send or receive a large number of Edge-Hello packets.
To reduce Edge-Hello traffic, perform the following tasks:
· Assign Ring 2 and Ring 3 to an RRPP ring group configured on the edge node Device B.
· Assign Ring 2 and Ring 3 to an RRPP ring group configured on the assistant edge node Device C.
If all rings are activated, only Ring 2 on Device B sends Edge-Hello packets.
Typical RRPP networking
Single ring
As shown in Figure 2, only a single ring exists in the network topology. You need only define an RRPP domain.
Figure 2 Schematic diagram for a single-ring network
Tangent rings
As shown in Figure 3, two or more rings exist in the network topology and only one common node exists between rings. You must define an RRPP domain for each ring.
Figure 3 Schematic diagram for a tangent-ring network
Intersecting rings
As shown in Figure 4, two or more rings exist in the network topology and two common nodes exist between rings. You need only define an RRPP domain and configure one ring as the primary ring and the other rings as subrings.
Figure 4 Schematic diagram for an intersecting-ring network
Dual-homed rings
As shown in Figure 5, two or more rings exist in the network topology and two similar common nodes exist between rings. You need only define an RRPP domain and configure one ring as the primary ring and the other rings as subrings.
Figure 5 Schematic diagram for a dual-homed-ring network
Single-ring load balancing
In a single-ring network, you can achieve load balancing by configuring multiple domains.
As shown in Figure 6:
· Ring 1 is configured as the primary ring of both Domain 1 and Domain 2.
· Domain 1 and Domain 2 are configured with different protected VLANs.
· In Domain 1, Device A is configured as the master node of Ring 1.
· In Domain 2, Device B is configured as the master node of Ring 1.
Such configurations enable the ring to block different links based on VLANs and achieve single-ring load balancing.
Figure 6 Schematic diagram for a single-ring load balancing network
Intersecting-ring load balancing
As shown in Figure 7:
· Ring 1 is the primary ring and Ring 2 is the subring in both Domain 1 and Domain 2.
· Device A is configured as the master node of Ring 1 in Domain 1.
· Device D is configured as the master node of Ring 1 in Domain 2.
· Device E is configured as the master node of Ring 2 in both Domain 1 and Domain 2. However, different ports on Device E are blocked in Domain 1 and Domain 2.
Traffic from different VLANs can travel over different paths in the subring and primary ring.
Figure 7 Schematic diagram for an intersecting-ring load balancing network
RRPP with M-LAG
M-LAG allows you to virtualize the devices in an RRPP ring into one system through multichassis link, thereby achieving device-level redundancy and load balancing.
As shown in Figure 8, the M-LAG system composed of Device A and Device E is the master node of Ring 1, and the M-LAG system composed of Device B and Device F is the transit node of Ring 1. For more information about M-LAG, see Layer 2—LAN Switching Configuration Guide.
Figure 8 RRPP with M-LAG
Protocols and standards
RFC 3619, Extreme Networks' Ethernet Automatic Protection Switching (EAPS) Version 1
· RRPP does not have an auto election mechanism. You must configure each node in the ring network correctly for RRPP to monitor and protect the ring network.
· You can configure RRPP in the following order:
¡ Create RRPP domains based on service planning.
¡ Specify control VLANs and protected VLANs for each RRPP domain.
¡ Determine the ring roles and node roles based on the traffic paths in each RRPP domain.
RRPP tasks at a glance
To configure RRPP, perform the following tasks:
Perform this task on devices you want to configure as nodes in the RRPP domain.
Perform this task on all nodes in the RRPP domain.
3. Configuring protected VLANs
Perform this task on each node's ports intended for accessing RRPP rings.
6. (Optional.) Configuring RRPP timers
Perform this task on the master node in the RRPP domain.
¡ Configuring the Hello timer and Fail timer
¡ Configuring the link-up delay timer
7. (Optional.) Configuring an RRPP ring group
Perform this task on the edge node and assistant edge node in the RRPP domain.
8. (Optional.) Enabling SNMP notifications for RRPP
Prerequisites for RRPP
Before you configure RRPP, you must physically construct a ring-shaped Ethernet topology.
Creating an RRPP domain
When you create an RRPP domain, specify a domain ID to uniquely identify the RRPP domain. All devices in the same RRPP domain must be configured with the same domain ID.
1. Enter system view.
2. Create an RRPP domain and enter RRPP domain view.
rrpp domain domain-id
Configuring control VLANs
· Perform this task on all nodes in the RRPP domain.
· Before you configure RRPP rings in an RRPP domain, configure the same control VLANs for all nodes in the RRPP domain first. You need only configure the primary control VLAN for an RRPP domain. The system automatically configures the secondary control VLAN. It uses the primary control VLAN ID plus 1 as the secondary control VLAN ID. For the control VLAN configuration to succeed, make sure the IDs of the two control VLANs are consecutive and have not been previously assigned.
· Do not configure the default VLAN of a port accessing an RRPP ring as the control VLAN.
· A VLAN with VLAN interface resource reservation cannot be configured as the control VLAN. For more information about VLAN interface resource reservation, see Layer 2—LAN Switching Configuration Guide.
· For RRPPDUs to be correctly forwarded, do not enable QinQ or VLAN mapping on control VLANs.
· After you configure RRPP rings for an RRPP domain, you cannot delete or modify the primary control VLAN of the domain. You can only use the undo control-vlan command to delete a primary control VLAN.
· To transparently transmit RRPPDUs on a device not configured with RRPP, make sure only the two ports accessing the RRPP ring permit packets from the control VLANs. Otherwise, the packets from other VLANs might enter the control VLANs in transparent transmission mode and strike the RRPP ring.
· When configuring RRPP with M-LAG, make sure the peer-link interface is a trunk port. The peer-link interface will automatically join or leave a control VLAN as the control VLAN is created or deleted.
2. Enter RRPP domain view.
3. Configure the primary control VLAN for the RRPP domain.
control-vlan vlan-id
· Before you configure RRPP rings in an RRPP domain, configure the same protected VLANs for all nodes in the RRPP domain. All VLANs to which the RRPP ports are assigned must be protected by the RRPP domains.
· When you configure load balancing, you must configure different protected VLANs for different RRPP domains.
Before you configure protected VLANs, you must configure an MST region and the VLAN-to-instance mapping table. For more information about MST regions, see spanning tree configuration in Layer 2—LAN Switching Configuration Guide.
3. Configure protected VLANs for the RRPP domain.
Configuring RRPP rings
When you configure an RRPP ring, you must configure the ports connecting each node to the RRPP ring before configuring the nodes.
Before you configure an RRPP ring, you must configure control VLANs and protected VLANs.
Configuring RRPP ports
· Perform this task on each node's ports intended for accessing RRPP rings.
· Do not enable the OAM remote loopback function on an RRPP port. Otherwise, temporary broadcast storms might occur.
· To accelerate topology convergence, use the link-delay command to enable link status rapid report function on an RRPP port. Use this command to set the physical state change suppression interval to 0 seconds. For more information about the link-delay command, see Interface Command Reference.
· Do not assign a port to both an aggregation group and an RRPP ring. If you do so, the port does not take effect on the RRPP ring.
· Do not assign a peer-link interface to an RRPP ring. A peer-link interface does not work for an RRPP ring.
· Do not assign both an M-LAG interface and a non-M-LAG interface to an RRPP ring. If you do so, the M-LAG interface does not take effect on the RRPP ring.
2. Enter Layer 2 Ethernet interface view or Layer 2 aggregate interface view.
3. Configure the link type of the interface as trunk.
port link-type trunk
By default, the link type of an interface is access.
For more information about the command, see Layer 2—LAN Switching Command Reference.
4. Assign the trunk port to the protected VLANs of the RRPP domain.
By default, a trunk port allows only packets from VLAN 1 to pass through.
RRPP ports always allow packets from the control VLANs to pass through.
5. Disable the spanning tree feature.
undo stp enable
By default, the spanning tree feature is enabled.
Configuring RRPP nodes
· If a device carries multiple RRPP rings in an RRPP domain, it can only be an edge node or an assistant edge node on a subring.
· When you configure an edge node or an assistant edge node, you must configure the primary ring before configuring the subrings.
Specifying a master node
3. Specify the current device as the master node of the ring, and specify the primary port and the secondary port.
ring ring-id node-mode master [ primary-port interface-type interface-number ] [ secondary-port interface-type interface-number ] level level-value
Specifying a transit node
3. Specify the current device as a transit node of the ring, and specify the primary port and the secondary port.
ring ring-id node-mode transit [ primary-port interface-type interface-number ] [ secondary-port interface-type interface-number ] level level-value
Specifying an edge node
3. Specify the current device as a master node or transit node of the primary ring, and specify the primary port and the secondary port.
ring ring-id node-mode { master | transit } [ primary-port interface-type interface-number ] [ secondary-port interface-type interface-number ] level level-value
4. Specify the current device as the edge node of a subring, and specify the edge port.
ring ring-id node-mode edge [ edge-port interface-type interface-number ]
Specifying an assistant edge node
By default, a device is not a node of the RRPP ring.
4. Specify the current device as the assistant edge node of the subring, and specify an edge port.
ring ring-id node-mode assistant-edge [ edge-port interface-type interface-number ]
Activating an RRPP domain
· Before you activate an RRPP domain on the current device, enable the RRPP protocol and RRPP rings for the RRPP domain on the current device.
· Before you enable subrings on a device, you must enable the primary ring. Before you disable the primary ring on the device, you must disable all subrings. Otherwise, the system displays error prompts.
· To prevent Hello packets of subrings from being looped on the primary ring, enable the primary ring on its master node first. Then enable the subrings on their respective master nodes.
2. Enable RRPP.
rrpp enable
By default, RRPP is disabled.
3. Enter RRPP domain view.
4. Enable the specified RRPP ring.
ring ring-id enable
By default, an RRPP ring is disabled.
Perform this task on the master node of an RRPP domain.
· The Fail timer must be greater than or equal to three times the Hello timer.
· In a dual-homed-ring network, to avoid temporary loops when the primary ring fails, make sure the value of A is greater than the value of B, where:
¡ A is the difference between the Fail timer values on the master node of the subring and the master node of the primary ring.
¡ B is twice the Hello timer value on the master node of the subring.
3. Set the Hello timer and Fail timer for the RRPP domain.
timer hello-timer hello-value fail-timer fail-value
By default, the Hello timer value is 1 second and the Fail timer value is 3 seconds.
If the distribute keyword is not specified, the link-up delay timer value cannot be greater than the Fail timer value minus twice the Hello timer value.
If you specify the distribute keyword in an RRPP network implementing load balancing, you must configure the link-up delay timer for each RRPP domain for the timer to take effect. If you set different timer values for different RRPP domains, the smallest timer value takes effect.
3. Set the link-up delay timer for the RRPP domain.
linkup-delay-timer delay-time [ distribute ]
By default, the link-up delay timer value is 0 seconds, and the distribute keyword is not specified.
To reduce Edge-Hello traffic, assign subrings with the same edge node and assistant edge node to an RRPP ring group. An RRPP ring group must be configured on both the edge node and the assistant edge node. It can only be configured on these two types of nodes.
· Perform this task on the edge node and assistant edge node in the RRPP domain.
· You can assign a subring to only one RRPP ring group. The RRPP ring groups configured on the edge node and the assistant edge node must contain the same subrings. Otherwise, the RRPP ring group cannot operate correctly.
· The subrings in an RRPP ring group must share the same edge node and assistant edge node. The edge node and the assistant edge node must have the same SRPTs.
· Make sure a device is either the edge node or the assistant edge node on the subrings in an RRPP ring group.
· Make sure the RRPP ring groups on the edge node and the assistant edge node have the same configurations and activation status.
· Make sure all subrings in an RRPP ring group have the same SRPTs. If the SRPTs of these subrings are different, the RRPP ring group cannot operate correctly.
2. Create an RRPP ring group and enter RRPP ring group view.
rrpp ring-group ring-group-id
By default, no RRPP ring groups exist.
3. Assign the specified subrings to the RRPP ring group.
domain domain-id ring ring-id-list
By default, no subrings are assigned to an RRPP ring group.
To report critical RRPP events to an NMS, enable SNMP notifications for RRPP. For RRPP event notifications to be sent correctly, you must also configure SNMP on the device. For more information about SNMP configuration, see the network management and monitoring configuration guide for the device.
2. Enable SNMP notifications for RRPP.
snmp-agent trap enable rrpp [ major-fault | multi-master | ring-fail | ring-recover ] *
By default, SNMP notifications for RRPP are disabled.
Task |
Command |
Display brief RRPP information. |
display rrpp brief |
Display RRPP group configuration information. |
display rrpp ring-group [ ring-group-id ] |
Display RRPPDU statistics. |
display rrpp statistics domain domain-id [ ring ring-id ] |
Display detailed RRPP information. |
display rrpp verbose domain domain-id [ ring ring-id ] |
Clear RRPPDU statistics. |
reset rrpp statistics domain domain-id [ ring ring-id ] |
RRPP configuration examples
As shown in Figure 9:
· Device A, Device B, Device C, and Device D form RRPP domain 1. Specify the primary control VLAN of RRPP domain 1 as VLAN 4092. Specify the protected VLANs of RRPP domain 1 as VLANs 1 through 30.
· Device A, Device B, Device C, and Device D form primary ring 1.
· Specify Device A as the master node of primary ring 1, Ten-GigabitEthernet 3/0/1 as the primary port, and Ten-GigabitEthernet 3/0/2 as the secondary port.
· Specify Device B, Device C, and Device D as the transit nodes of primary ring 1. Specify Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port on Device B, Device C, and Device D.
1. Configure Device A:
# Create VLANs 1 through 30.
[DeviceA] vlan 1 to 30
# Map these VLANs to MSTI 1.
[DeviceA] stp region-configuration
[DeviceA-mst-region] instance 1 vlan 1 to 30
# Activate the MST region configuration.
[DeviceA-mst-region] active region-configuration
[DeviceA-mst-region] quit
# Set the physical state change suppression interval to 0 seconds on Ten-GigabitEthernet 3/0/1.
[DeviceA] interface ten-gigabitethernet 3/0/1
[DeviceA-Ten-GigabitEthernet3/0/1] link-delay up 0
[DeviceA-Ten-GigabitEthernet3/0/1] link-delay down 0
# Disable the spanning tree feature on the port.
[DeviceA-Ten-GigabitEthernet3/0/1] undo stp enable
# Configure the port as a trunk port.
[DeviceA-Ten-GigabitEthernet3/0/1] port link-type trunk
# Assign the port to VLANs 1 through 30.
[DeviceA-Ten-GigabitEthernet3/0/1] port trunk permit vlan 1 to 30
[DeviceA-Ten-GigabitEthernet3/0/1] quit
# Configure Ten-GigabitEthernet 3/0/2 in the same way Ten-GigabitEthernet 3/0/1 is configured.
[DeviceA] interface ten-gigabitethernet 3/0/2
[DeviceA-Ten-GigabitEthernet3/0/2] link-delay up 0
[DeviceA-Ten-GigabitEthernet3/0/2] link-delay down 0
[DeviceA-Ten-GigabitEthernet3/0/2] undo stp enable
[DeviceA-Ten-GigabitEthernet3/0/2] port link-type trunk
[DeviceA-Ten-GigabitEthernet3/0/2] port trunk permit vlan 1 to 30
[DeviceA-Ten-GigabitEthernet3/0/2] quit
# Create RRPP domain 1.
[DeviceA] rrpp domain 1
# Configure VLAN 4092 as the primary control VLAN of RRPP domain 1.
[DeviceA-rrpp-domain1] control-vlan 4092
# Configure the VLANs mapped to MSTI 1 as the protected VLANs of RRPP domain 1.
[DeviceA-rrpp-domain1] protected-vlan reference-instance 1
# Configure Device A as the master node of primary ring 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
[DeviceA-rrpp-domain1] ring 1 node-mode master primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 0
[DeviceA-rrpp-domain1] ring 1 enable
[DeviceA-rrpp-domain1] quit
# Enable RRPP.
[DeviceA] rrpp enable
2. Configure Device B:
[DeviceB] vlan 1 to 30
[DeviceB] stp region-configuration
[DeviceB-mst-region] instance 1 vlan 1 to 30
[DeviceB-mst-region] active region-configuration
[DeviceB-mst-region] quit
[DeviceB] interface ten-gigabitethernet 3/0/1
[DeviceB-Ten-GigabitEthernet3/0/1] link-delay up 0
[DeviceB-Ten-GigabitEthernet3/0/1] link-delay down 0
[DeviceB-Ten-GigabitEthernet3/0/1] undo stp enable
[DeviceB-Ten-GigabitEthernet3/0/1] port link-type trunk
[DeviceB-Ten-GigabitEthernet3/0/1] port trunk permit vlan 1 to 30
[DeviceB-Ten-GigabitEthernet3/0/1] quit
[DeviceB] interface ten-gigabitethernet 3/0/2
[DeviceB-Ten-GigabitEthernet3/0/2] link-delay up 0
[DeviceB-Ten-GigabitEthernet3/0/2] link-delay down 0
[DeviceB-Ten-GigabitEthernet3/0/2] undo stp enable
[DeviceB-Ten-GigabitEthernet3/0/2] port link-type trunk
[DeviceB-Ten-GigabitEthernet3/0/2] port trunk permit vlan 1 to 30
[DeviceB-Ten-GigabitEthernet3/0/2] quit
[DeviceB] rrpp domain 1
[DeviceB-rrpp-domain1] control-vlan 4092
[DeviceB-rrpp-domain1] protected-vlan reference-instance 1
# Configure Device B as the transit node of primary ring 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
[DeviceB-rrpp-domain1] ring 1 node-mode transit primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 0
[DeviceB-rrpp-domain1] ring 1 enable
[DeviceB-rrpp-domain1] quit
# Enable RRPP.
[DeviceB] rrpp enable
3. Configure Device C:
Configure Device C in the same way Device B is configured.
4. Configure Device D:
Configure Device D in the same way Device B is configured.
# Use the display commands to view RRPP configuration and operational information on each device.
As shown in Figure 10:
· Device A, Device B, Device C, Device D, and Device E form RRPP domain 1. VLAN 4092 is the primary control VLAN of RRPP domain 1. RRPP domain 1 protects VLANs 1 through 30.
· Device A, Device B, Device C, and Device D form primary ring 1. Device B, Device C, and Device E form subring 2.
· Device A is the master node of primary ring 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 the secondary port.
· Device E is the master node of subring 2, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 the secondary port.
· Device B is the transit node of primary ring 1 and the edge node of subring 2, with Ten-GigabitEthernet 3/0/3 as the edge port.
· Device C is the transit node of primary ring 1 and the assistant edge node of subring 1, with Ten-GigabitEthernet 3/0/3 as the edge port.
· Device D is the transit node of primary ring 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 the secondary port.
# Enable RRPP.
# Configure Ten-GigabitEthernet 3/0/3 in the same way Ten-GigabitEthernet 3/0/1 is configured.
[DeviceB] interface ten-gigabitethernet 3/0/3
[DeviceB-Ten-GigabitEthernet3/0/3] link-delay up 0
[DeviceB-Ten-GigabitEthernet3/0/3] undo stp enable
[DeviceB-Ten-GigabitEthernet3/0/3] port link-type trunk
[DeviceB-Ten-GigabitEthernet3/0/3] port trunk permit vlan 1 to 30
[DeviceB-Ten-GigabitEthernet3/0/3] quit
# Configure Device B as a transit node of primary ring 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
# Configure Device B as the edge node of subring 2, with Ten-GigabitEthernet 3/0/3 as the edge port. Enable ring 2.
[DeviceB-rrpp-domain1] ring 2 node-mode edge edge-port ten-gigabitethernet 3/0/3
[DeviceB-rrpp-domain1] ring 2 enable
# Enable RRPP.
<DeviceC> system-view
[DeviceC] vlan 1 to 30
[DeviceC-mst-region] instance 1 vlan 1 to 30
[DeviceC-mst-region] quit
[DeviceC] interface ten-gigabitethernet 3/0/1
[DeviceC-Ten-GigabitEthernet3/0/1] link-delay up 0
[DeviceC-Ten-GigabitEthernet3/0/1] link-delay down 0
[DeviceC-Ten-GigabitEthernet3/0/1] undo stp enable
[DeviceC-Ten-GigabitEthernet3/0/1] port link-type trunk
[DeviceC-Ten-GigabitEthernet3/0/1] port trunk permit vlan 1 to 30
[DeviceC-Ten-GigabitEthernet3/0/1] quit
[DeviceC] interface ten-gigabitethernet 3/0/2
[DeviceC-Ten-GigabitEthernet3/0/2] link-delay up 0
[DeviceC-Ten-GigabitEthernet3/0/2] link-delay down 0
[DeviceC-Ten-GigabitEthernet3/0/2] undo stp enable
[DeviceC-Ten-GigabitEthernet3/0/2] port link-type trunk
[DeviceC-Ten-GigabitEthernet3/0/2] port trunk permit vlan 1 to 30
[DeviceC-Ten-GigabitEthernet3/0/2] quit
[DeviceC] interface ten-gigabitethernet 3/0/3
[DeviceC-Ten-GigabitEthernet3/0/3] link-delay up 0
[DeviceC-Ten-GigabitEthernet3/0/3] link-delay down 0
[DeviceC-Ten-GigabitEthernet3/0/3] undo stp enable
[DeviceC-Ten-GigabitEthernet3/0/3] port link-type trunk
[DeviceC-Ten-GigabitEthernet3/0/3] port trunk permit vlan 1 to 30
[DeviceC-Ten-GigabitEthernet3/0/3] quit
[DeviceC] rrpp domain 1
[DeviceC-rrpp-domain1] control-vlan 4092
[DeviceC-rrpp-domain1] protected-vlan reference-instance 1
# Configure Device C as a transit node of primary ring 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
[DeviceC-rrpp-domain1] ring 1 node-mode transit primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 0
[DeviceC-rrpp-domain1] ring 1 enable
# Configure Device C as the assistant edge node of subring 2, with Ten-GigabitEthernet 3/0/3 as the edge port. Enable ring 2.
[DeviceC-rrpp-domain1] ring 2 node-mode assistant-edge edge-port ten-gigabitethernet 3/0/3
[DeviceC-rrpp-domain1] ring 2 enable
[DeviceC-rrpp-domain1] quit
# Enable RRPP.
[DeviceC] rrpp enable
<DeviceD> system-view
[DeviceD] vlan 1 to 30
[DeviceD-mst-region] instance 1 vlan 1 to 30
[DeviceD-mst-region] quit
[DeviceD] interface ten-gigabitethernet 3/0/1
[DeviceD-Ten-GigabitEthernet3/0/1] link-delay up 0
[DeviceD-Ten-GigabitEthernet3/0/1] link-delay down 0
[DeviceD-Ten-GigabitEthernet3/0/1] undo stp enable
[DeviceD-Ten-GigabitEthernet3/0/1] port link-type trunk
[DeviceD-Ten-GigabitEthernet3/0/1] port trunk permit vlan 1 to 30
[DeviceD-Ten-GigabitEthernet3/0/1] quit
[DeviceD] interface ten-gigabitethernet 3/0/2
[DeviceD-Ten-GigabitEthernet3/0/2] link-delay up 0
[DeviceD-Ten-GigabitEthernet3/0/2] link-delay down 0
[DeviceD-Ten-GigabitEthernet3/0/2] undo stp enable
[DeviceD-Ten-GigabitEthernet3/0/2] port link-type trunk
[DeviceD-Ten-GigabitEthernet3/0/2] port trunk permit vlan 1 to 30
[DeviceD-Ten-GigabitEthernet3/0/2] quit
[DeviceD] rrpp domain 1
[DeviceD-rrpp-domain1] control-vlan 4092
[DeviceD-rrpp-domain1] protected-vlan reference-instance 1
# Configure Device D as the transit node of primary ring 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
[DeviceD-rrpp-domain1] ring 1 node-mode transit primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 0
[DeviceD-rrpp-domain1] ring 1 enable
[DeviceD-rrpp-domain1] quit
# Enable RRPP.
[DeviceD] rrpp enable
5. Configure Device E:
<DeviceE> system-view
[DeviceE] vlan 1 to 30
[DeviceE] stp region-configuration
[DeviceE-mst-region] instance 1 vlan 1 to 30
[DeviceE-mst-region] active region-configuration
[DeviceE-mst-region] quit
[DeviceE] interface ten-gigabitethernet 3/0/1
[DeviceE-Ten-GigabitEthernet3/0/1] link-delay up 0
[DeviceE-Ten-GigabitEthernet3/0/1] link-delay down 0
[DeviceE-Ten-GigabitEthernet3/0/1] undo stp enable
[DeviceE-Ten-GigabitEthernet3/0/1] port link-type trunk
[DeviceE-Ten-GigabitEthernet3/0/1] port trunk permit vlan 1 to 30
[DeviceE-Ten-GigabitEthernet3/0/1] quit
[DeviceE] interface ten-gigabitethernet 3/0/2
[DeviceE-Ten-GigabitEthernet3/0/2] link-delay up 0
[DeviceE-Ten-GigabitEthernet3/0/2] link-delay down 0
[DeviceE-Ten-GigabitEthernet3/0/2] undo stp enable
[DeviceE-Ten-GigabitEthernet3/0/2] port link-type trunk
[DeviceE-Ten-GigabitEthernet3/0/2] port trunk permit vlan 1 to 30
[DeviceE-Ten-GigabitEthernet3/0/2] quit
[DeviceE] rrpp domain 1
[DeviceE-rrpp-domain1] control-vlan 4092
[DeviceE-rrpp-domain1] protected-vlan reference-instance 1
# Configure Device E as the master node of subring 2, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 2.
[DeviceE-rrpp-domain1] ring 2 node-mode master primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 1
[DeviceE-rrpp-domain1] ring 2 enable
[DeviceE-rrpp-domain1] quit
# Enable RRPP.
[DeviceE] rrpp enable
As shown in Figure 11:
· Device A, Device B, Device C, Device D, and Device F form RRPP domain 1. VLAN 100 is the primary control VLAN of the RRPP domain. Device A is the master node of the primary ring, Ring 1. Device D is the transit node of Ring 1. Device F is the master node of the subring Ring 3. Device C is the edge node of the subring Ring 3. Device B is the assistant edge node of the subring Ring 3.
· Device A, Device B, Device C, Device D, and Device E form RRPP domain 2. VLAN 105 is the primary control VLAN of the RRPP domain. Device A is the master node of the primary ring, Ring 1. Device D is the transit node of Ring 1. Device E is the master node of the subring Ring 2. Device C is the edge node of the subring Ring 2. Device B is the assistant edge node of the subring Ring 2.
· Specify VLAN 11 as the protected VLAN of domain 1, and VLAN 12 the protected VLAN of domain 2. You can implement VLAN-based load balancing on Ring 1.
· Ring 2 and Ring 3 have the same edge node and assistant edge node, and the two subrings have the same SRPTs. You can add Ring 2 and Ring 3 to an RRPP ring group to reduce Edge-Hello traffic.
# Create VLANs 11 and 12.
[DeviceA] vlan 11 to 12
# Map VLAN 11 to MSTI 1 and VLAN 12 to MSTI 2.
[DeviceA-mst-region] instance 1 vlan 11
[DeviceA-mst-region] instance 2 vlan 12
# Remove the port from VLAN 1, and assign it to VLANs 11 and 12.
[DeviceA-Ten-GigabitEthernet3/0/1] undo port trunk permit vlan 1
[DeviceA-Ten-GigabitEthernet3/0/1] port trunk permit vlan 11 12
# Configure VLAN 11 as the default VLAN.
[DeviceA-Ten-GigabitEthernet3/0/1] port trunk pvid vlan 11
[DeviceA-Ten-GigabitEthernet3/0/2] undo port trunk permit vlan 1
[DeviceA-Ten-GigabitEthernet3/0/2] port trunk permit vlan 11 12
[DeviceA-Ten-GigabitEthernet3/0/2] port trunk pvid vlan 11
# Configure VLAN 100 as the primary control VLAN of RRPP domain 1.
[DeviceA-rrpp-domain1] control-vlan 100
# Configure the VLAN mapped to MSTI 1 as the protected VLAN of RRPP domain 1.
# Create RRPP domain 2.
[DeviceA] rrpp domain 2
# Configure VLAN 105 as the primary control VLAN of RRPP domain 2.
[DeviceA-rrpp-domain2] control-vlan 105
# Configure the VLAN mapped to MSTI 2 as the protected VLAN of RRPP domain 2.
[DeviceA-rrpp-domain2] protected-vlan reference-instance 2
# Configure Device A as the master node of primary ring 1, with Ten-GigabitEthernet 3/0/2 as the master port and Ten-GigabitEthernet 3/0/1 as the secondary port. Enable ring 1.
[DeviceA-rrpp-domain2] ring 1 node-mode master primary-port ten-gigabitethernet 3/0/2 secondary-port ten-gigabitethernet 3/0/1 level 0
[DeviceA-rrpp-domain2] ring 1 enable
[DeviceA-rrpp-domain2] quit
# Enable RRPP.
[DeviceB] vlan 11 to 12
[DeviceB-mst-region] instance 1 vlan 11
[DeviceB-mst-region] instance 2 vlan 12
[DeviceB-Ten-GigabitEthernet3/0/1] undo port trunk permit vlan 1
[DeviceB-Ten-GigabitEthernet3/0/1] port trunk permit vlan 11 12
[DeviceB-Ten-GigabitEthernet3/0/1] port trunk pvid vlan 11
[DeviceB-Ten-GigabitEthernet3/0/2] undo port trunk permit vlan 1
[DeviceB-Ten-GigabitEthernet3/0/2] port trunk permit vlan 11 12
[DeviceB-Ten-GigabitEthernet3/0/2] port trunk pvid vlan 11
# Set the physical state change suppression interval to 0 seconds on Ten-GigabitEthernet 3/0/3.
[DeviceB-Ten-GigabitEthernet3/0/3] link-delay down 0
# Remove the port from VLAN 1, and assign it to VLAN 12.
[DeviceB-Ten-GigabitEthernet3/0/3] undo port trunk permit vlan 1
[DeviceB-Ten-GigabitEthernet3/0/3] port trunk permit vlan 12
# Configure VLAN 12 as the default VLAN.
[DeviceB-Ten-GigabitEthernet3/0/3] port trunk pvid vlan 12
# Set the physical state change suppression interval to 0 seconds on Ten-GigabitEthernet 3/0/4.
[DeviceB] interface ten-gigabitethernet 3/0/4
[DeviceB-Ten-GigabitEthernet3/0/4] link-delay up 0
[DeviceB-Ten-GigabitEthernet3/0/4] link-delay down 0
[DeviceB-Ten-GigabitEthernet3/0/4] undo stp enable
[DeviceB-Ten-GigabitEthernet3/0/4] port link-type trunk
# Remove the port from VLAN 1, and assign it to VLAN 11.
[DeviceB-Ten-GigabitEthernet3/0/4] undo port trunk permit vlan 1
[DeviceB-Ten-GigabitEthernet3/0/4] port trunk permit vlan 11
[DeviceB-Ten-GigabitEthernet3/0/4] port trunk pvid vlan 11
[DeviceB-Ten-GigabitEthernet3/0/4] quit
[DeviceB-rrpp-domain1] control-vlan 100
# Configure Device B as a transit node of primary ring 1 in RRPP domain 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
# Configure Device B as the assistant edge node of subring 3 in RRPP domain 1, with Ten-GigabitEthernet 3/0/4 as the edge port. Enable subring 3.
[DeviceB-rrpp-domain1] ring 3 node-mode assistant-edge edge-port ten-gigabitethernet 3/0/4
[DeviceB-rrpp-domain1] ring 3 enable
[DeviceB] rrpp domain 2
[DeviceB-rrpp-domain2] control-vlan 105
[DeviceB-rrpp-domain2] protected-vlan reference-instance 2
[DeviceB-rrpp-domain2] ring 1 node-mode transit primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 0
[DeviceB-rrpp-domain2] ring 1 enable
# Configure Device B as the assistant edge node of subring 2 in RRPP domain 2, with Ten-GigabitEthernet 3/0/3 as the edge port. Enable subring 2.
[DeviceB-rrpp-domain2] ring 2 node-mode assistant-edge edge-port ten-gigabitethernet 3/0/3
[DeviceB-rrpp-domain2] ring 2 enable
[DeviceC-rrpp-domain2] quit
# Enable RRPP.
[DeviceC] vlan 11 to 12
[DeviceC-mst-region] instance 1 vlan 11
[DeviceC-mst-region] instance 2 vlan 12
[DeviceC-Ten-GigabitEthernet3/0/1] undo port trunk permit vlan 1
[DeviceC-Ten-GigabitEthernet3/0/1] port trunk permit vlan 11 12
[DeviceC-Ten-GigabitEthernet3/0/1] port trunk pvid vlan 11
[DeviceC-Ten-GigabitEthernet3/0/2] undo port trunk permit vlan 1
[DeviceC-Ten-GigabitEthernet3/0/2] port trunk permit vlan 11 12
[DeviceC-Ten-GigabitEthernet3/0/2] port trunk pvid vlan 11
[DeviceC-Ten-GigabitEthernet3/0/3] undo port trunk permit vlan 1
[DeviceC-Ten-GigabitEthernet3/0/3] port trunk permit vlan 12
[DeviceC-Ten-GigabitEthernet3/0/3] port trunk pvid vlan 12
[DeviceC] interface ten-gigabitethernet 3/0/4
[DeviceC-Ten-GigabitEthernet3/0/4] link-delay up 0
[DeviceC-Ten-GigabitEthernet3/0/4] link-delay down 0
[DeviceC-Ten-GigabitEthernet3/0/4] undo stp enable
[DeviceC-Ten-GigabitEthernet3/0/4] port link-type trunk
[DeviceC-Ten-GigabitEthernet3/0/4] undo port trunk permit vlan 1
[DeviceC-Ten-GigabitEthernet3/0/4] port trunk permit vlan 11
[DeviceC-Ten-GigabitEthernet3/0/4] port trunk pvid vlan 11
[DeviceC-Ten-GigabitEthernet3/0/4] quit
[DeviceC-rrpp-domain1] control-vlan 100
# Configure Device C as the transit node of primary ring 1 in RRPP domain 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
# Configure Device C as the edge node of subring 3 in RRPP domain 1, with Ten-GigabitEthernet 3/0/4 as the edge port. Enable subring 3.
[DeviceC-rrpp-domain1] ring 3 node-mode edge edge-port ten-gigabitethernet 3/0/4
[DeviceC-rrpp-domain1] ring 3 enable
[DeviceC] rrpp domain 2
[DeviceC-rrpp-domain2] control-vlan 105
[DeviceC-rrpp-domain2] protected-vlan reference-instance 2
# Configure Device C as the transit node of primary ring 1 in RRPP domain 2, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
[DeviceC-rrpp-domain2] ring 1 node-mode transit primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 0
[DeviceC-rrpp-domain2] ring 1 enable
# Configure Device C as the edge node of subring 2 in RRPP domain 2, with Ten-GigabitEthernet 3/0/3 as the edge port. Enable subring 2.
[DeviceC-rrpp-domain2] ring 2 node-mode edge edge-port ten-gigabitethernet 3/0/3
[DeviceC-rrpp-domain2] ring 2 enable
# Enable RRPP.
[DeviceD] vlan 11 to 12
[DeviceD-mst-region] instance 1 vlan 11
[DeviceD-mst-region] instance 2 vlan 12
[DeviceD-Ten-GigabitEthernet3/0/1] undo port trunk permit vlan 1
[DeviceD-Ten-GigabitEthernet3/0/1] port trunk permit vlan 11 12
[DeviceD-Ten-GigabitEthernet3/0/1] port trunk pvid vlan 11
[DeviceD-Ten-GigabitEthernet3/0/2] undo port trunk permit vlan 1
[DeviceD-Ten-GigabitEthernet3/0/2] port trunk permit vlan 11 12
[DeviceD-Ten-GigabitEthernet3/0/2] port trunk pvid vlan 11
[DeviceD-rrpp-domain1] control-vlan 100
# Configure Device D as the transit node of primary ring 1 in RRPP domain 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
[DeviceD] rrpp domain 2
[DeviceD-rrpp-domain2] control-vlan 105
[DeviceD-rrpp-domain2] protected-vlan reference-instance 2
# Configure Device D as the transit node of primary ring 1 in RRPP domain 2, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable ring 1.
[DeviceD-rrpp-domain2] ring 1 node-mode transit primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 0
[DeviceD-rrpp-domain2] ring 1 enable
[DeviceD-rrpp-domain2] quit
# Enable RRPP.
# Create VLAN 12.
[DeviceE] vlan 12
# Map VLAN 12 to MSTI 2.
[DeviceE-vlan12] quit
[DeviceE-mst-region] instance 2 vlan 12
[DeviceE-Ten-GigabitEthernet3/0/1] undo port trunk permit vlan 1
[DeviceE-Ten-GigabitEthernet3/0/1] port trunk permit vlan 12
[DeviceE-Ten-GigabitEthernet3/0/1] port trunk pvid vlan 12
[DeviceE-Ten-GigabitEthernet3/0/2] undo port trunk permit vlan 1
[DeviceE-Ten-GigabitEthernet3/0/2] port trunk permit vlan 12
[DeviceE-Ten-GigabitEthernet3/0/2] port trunk pvid vlan 12
[DeviceE] rrpp domain 2
[DeviceE-rrpp-domain2] control-vlan 105
[DeviceE-rrpp-domain2] protected-vlan reference-instance 2
# Configure Device E as the master mode of subring 2 in RRPP domain 2, with Ten-GigabitEthernet 3/0/2 as the primary port and Ten-GigabitEthernet 3/0/1 as the secondary port. Enable ring 2.
[DeviceE-rrpp-domain2] ring 2 node-mode master primary-port ten-gigabitethernet 3/0/2 secondary-port ten-gigabitethernet 3/0/1 level 1
[DeviceE-rrpp-domain2] ring 2 enable
[DeviceE-rrpp-domain2] quit
# Enable RRPP.
6. Configure Device F:
# Create VLAN 11.
<DeviceF> system-view
[DeviceF] vlan 11
[DeviceF-vlan11] quit
# Map VLAN 11 to MSTI 1.
[DeviceF] stp region-configuration
[DeviceF-mst-region] instance 1 vlan 11
[DeviceF-mst-region] active region-configuration
[DeviceF-mst-region] quit
[DeviceF] interface ten-gigabitethernet 3/0/1
[DeviceF-Ten-GigabitEthernet3/0/1] link-delay up 0
[DeviceF-Ten-GigabitEthernet3/0/1] link-delay down 0
[DeviceF-Ten-GigabitEthernet3/0/1] undo stp enable
[DeviceF-Ten-GigabitEthernet3/0/1] port link-type trunk
[DeviceF-Ten-GigabitEthernet3/0/1] undo port trunk permit vlan 1
[DeviceF-Ten-GigabitEthernet3/0/1] port trunk permit vlan 11
[DeviceF-Ten-GigabitEthernet3/0/1] port trunk pvid vlan 11
[DeviceF-Ten-GigabitEthernet3/0/1] quit
[DeviceF] interface ten-gigabitethernet 3/0/2
[DeviceF-Ten-GigabitEthernet3/0/2] link-delay up 0
[DeviceF-Ten-GigabitEthernet3/0/2] link-delay down 0
[DeviceF-Ten-GigabitEthernet3/0/2] undo stp enable
[DeviceF-Ten-GigabitEthernet3/0/2] port link-type trunk
[DeviceF-Ten-GigabitEthernet3/0/2] undo port trunk permit vlan 1
[DeviceF-Ten-GigabitEthernet3/0/2] port trunk permit vlan 11
[DeviceF-Ten-GigabitEthernet3/0/2] port trunk pvid vlan 11
[DeviceF-Ten-GigabitEthernet3/0/2] quit
[DeviceF] rrpp domain 1
[DeviceF-rrpp-domain1] control-vlan 100
[DeviceF-rrpp-domain1] protected-vlan reference-instance 1
# Configure Device F as the master node of subring 3 in RRPP domain 1, with Ten-GigabitEthernet 3/0/1 as the primary port and Ten-GigabitEthernet 3/0/2 as the secondary port. Enable subring 3.
[DeviceF-rrpp-domain1] ring 3 node-mode master primary-port ten-gigabitethernet 3/0/1 secondary-port ten-gigabitethernet 3/0/2 level 1
[DeviceF-rrpp-domain1] ring 3 enable
[DeviceF-rrpp-domain1] quit
# Enable RRPP.
[DeviceF] rrpp enable
7. Configure RRPP ring group settings on Device B and Device C:
# Create RRPP ring group 1 on Device B, and add subrings 2 and 3 to the RRPP ring group.
[DeviceB] rrpp ring-group 1
[DeviceB-rrpp-ring-group1] domain 2 ring 2
[DeviceB-rrpp-ring-group1] domain 1 ring 3
# Create RRPP ring group 1 on Device C, and add subrings 2 and 3 to the RRPP ring group.
[DeviceC] rrpp ring-group 1
[DeviceC-rrpp-ring-group1] domain 2 ring 2
[DeviceC-rrpp-ring-group1] domain 1 ring 3
Troubleshooting RRPP
Symptom
When the link state is normal, the master node cannot receive Hello packets, and it unblocks the secondary port.
Analysis
The following are possible causes:
· One or more nodes on the RRPP ring are not enabled with RRPP.
· The domain IDs or control VLANs are not the same for all nodes on the RRPP ring.
· The port on the RRPP ring does not work correctly.
Solution
To resolve the problem:
1. Use the display rrpp brief command to determine whether RRPP is enabled for all nodes. If it is not, use the rrpp enable command and the ring enable command to enable RRPP and RRPP rings for all nodes.
2. Use the display rrpp brief command to determine whether the domain ID and primary control VLAN ID are the same for all nodes. If they are not, set the same domain ID and primary control VLAN ID for the nodes.
3. Use the display rrpp verbose command to examine the link state of each port in each ring.
4. Use the debugging rrpp command on each node to determine whether a port receives or transmits Hello packets. If it does not, Hello packets are lost.
5. If the problem persists, contact H3C Support.
