HomeSupportConfigure & DeployConfiguration GuidesH3C S5135S-EI & S5136S-EI Switch Series Configuration Guide-R68xx-6W10109-Security Configuration Guide
17-ARP attack protection configuration
17-ARP attack protection configuration 362.94 KB
Configuring ARP attack protection· 1
About ARP attack protection· 1
ARP attack protection tasks at a glance· 1
Configuring unresolvable IP attack protection· 1
About unresolvable IP attack protection· 1
Configuring ARP source suppression· 2
Configuring ARP blackhole routing· 2
Display and maintenance commands for unresolvable IP attack protection· 3
Example: Configuring unresolvable IP attack protection· 3
Configuring ARP packet rate limit 4
Configuring source MAC-based ARP attack detection· 5
About this task· 5
Restrictions and guidelines· 6
Procedure· 6
Display and maintenance commands for source MAC-based ARP attack detection· 6
Example: Configuring source MAC-based ARP attack detection· 7
Configuring ARP packet source MAC consistency check· 8
About ARP packet source MAC consistency check· 8
Procedure· 8
Configuring ARP active acknowledgement 8
Configuring authorized ARP· 9
About authorized ARP· 9
Procedure· 9
Configuring ARP attack detection· 9
About ARP attack detection· 9
Restrictions and guidelines: ARP attack detection· 9
Configuring user validity check· 10
Configuring ARP packet validity check· 12
Configuring ARP restricted forwarding· 13
Ignoring ingress ports of ARP packets during user validity check· 14
Enabling ARP attack detection logging· 14
Display and maintenance commands for ARP attack detection· 14
Example: Configuring user validity check· 15
Example: Configuring user validity check and ARP packet validity check· 16
Example: Configuring ARP restricted forwarding· 17
Configuring ARP scanning and fixed ARP· 19
About this task· 19
Restrictions and guidelines· 19
Triggering ARP scanning· 20
Configuring automatic ARP scanning· 20
Configuring fixed ARP· 20
Configuring ARP keepalive entry scanning· 21
About ARP keepalive entry scanning· 21
Display and maintenance commands for ARP keepalive entry scanning· 21
Configuring ARP gateway protection· 22
About ARP gateway protection· 22
Restrictions and guidelines· 22
Procedure· 22
Example: Configuring ARP gateway protection· 22
Configuring ARP filtering· 23
About ARP filtering· 23
Restrictions and guidelines· 23
Procedure· 23
Example: Configuring ARP filtering· 24
Configuring ARP sender IP address checking· 25
About ARP sender IP address checking· 25
Procedure· 25
Enabling SNMP notifications for ARP· 25
The device can provide multiple features to detect and prevent ARP attacks and viruses in the LAN. An attacker can exploit ARP vulnerabilities to attack network devices in the following ways:
·     Sends a large number of unresolvable IP packets to have the receiving device busy with resolving IP addresses until its CPU is overloaded. Unresolvable IP packets refer to IP packets for which ARP cannot find corresponding MAC addresses.
·     Sends a large number of ARP packets to overload the CPU of the receiving device.
·     Acts as a trusted user or gateway to send ARP packets so the receiving devices obtain incorrect ARP entries.
All ARP attack protection tasks are optional.
·     Preventing flood attacks
¡     Configuring unresolvable IP attack protection
¡     Configuring ARP packet rate limit
¡     Configuring source MAC-based ARP attack detection
·     Preventing user and gateway spoofing attacks
¡     Configuring ARP packet source MAC consistency check
¡     Configuring ARP active acknowledgement
¡     Configuring authorized ARP
¡     Configuring ARP attack detection
¡     Configuring ARP packet validity check
¡     Configuring ARP restricted forwarding
¡     Ignoring ingress ports of ARP packets during user validity check
¡     Enabling ARP attack detection logging
¡     Configuring ARP scanning and fixed ARP
¡     Configuring ARP keepalive entry scanning
¡     Configuring ARP gateway protection
¡     Configuring ARP filtering
¡     Configuring ARP sender IP address checking
·     Enabling SNMP notifications for ARP
If a device receives a large number of unresolvable IP packets from a host, the following situations can occur:
·     The device sends a large number of ARP requests, overloading the target subnets.
·     The device keeps trying to resolve the destination IP addresses, overloading its CPU.
To protect the device from such IP attacks, you can configure the following features:
·     ARP source suppression—This feature is applicable if the attack packets have the same source addresses.
·     ARP blackhole routing—This feature is applicable regardless of whether the attack packets have the same source addresses.
This feature stops resolving packets from an IP address if the number of unresolvable IP packets from the IP address exceeds the upper limit within 5 seconds. The device continues ARP resolution when the interval elapses.
For a gateway or server trusted by the device, you can configure an ARP source suppression rule so that the device always permits IP packets sourced from the IP address of the gateway or server.
To have the configured ARP source suppression rules take effect, you must enable ARP source suppression by using the arp source-suppression enable command.
2.     Enable ARP source suppression.
By default, ARP source suppression is disabled.
3.     Set the maximum number of unresolvable packets that the device can process per source IP address within 5 seconds.
By default, the maximum number is 10.
4.     Configure ARP source suppression rules.
arp source-suppression rule rule-id permit ip-address [ mask ]
By default, no ARP source suppression rules exist.
This feature creates a blackhole route destined for an unresolved IP address. The device drops all matching packets until the blackhole route is deleted. A blackhole route is deleted when its aging timer is reached or the route becomes reachable.
After a blackhole route is created for an unresolved IP address, the device immediately starts the first ARP blackhole route probe by sending an ARP request. If the resolution fails, the device continues probing according to the probe settings. If the IP address resolution succeeds in a probe, the device converts the blackhole route to a normal route. If an ARP blackhole route ages out before the device finishes all probes, the device deletes the blackhole route and does not perform the remaining probes.
Set the ARP blackhole route probe count to a big value, for example, 25. If the device fails to reach the destination IP address temporarily and the probe count is too small, all probes might finish before the problem is resolved. As a result, non-attack packets will be dropped. This setting can avoid such situation.
2.     Enable ARP blackhole routing.
arp resolving-route enable
By default, ARP blackhole routing is enabled.
3.     (Optional.) Set the number of ARP blackhole route probes for each unresolved IP address.
arp resolving-route probe-count count
The default setting is three probes.
4.      (Optional.) Set the interval at which the device probes ARP blackhole routes.
arp resolving-route probe-interval interval
The default setting is 1 second.
Display ARP source suppression configuration information.
display arp source-suppression
Display ARP source suppression entries.
display arp source-suppression cache [ slot slot-number ]
As shown in Figure 1, a LAN contains two areas: an R&D area in VLAN 10 and an office area in VLAN 20. Each area connects to the gateway (Device) through an access switch.
A large number of ARP requests are detected in the office area and are considered an attack caused by unresolvable IP packets. To prevent the attack, configure ARP source suppression or ARP blackhole routing.
Figure 1 Network diagram
·     If the attack packets have the same source address, configure ARP source suppression:
# Enable ARP source suppression.
[Device] arp source-suppression enable
# Configure the device to process a maximum of 100 unresolvable packets per source IP address within 5 seconds.
[Device] arp source-suppression limit 100
·     If the attack packets have different source addresses, configure ARP blackhole routing:
# Enable ARP blackhole routing.
[Device] arp resolving-route enable
The ARP packet rate limit feature allows you to limit the rate of ARP packets delivered to the CPU. An ARP attack detection-enabled device will send all received ARP packets to the CPU for inspection. Processing excessive ARP packets will make the device malfunction or even crash. To solve this problem, configure ARP packet rate limit. When the receiving rate of ARP packets on the interface exceeds the rate limit, those packets are discarded.
You can enable sending notifications to the SNMP module or enable logging for ARP packet rate limit.
·     If notification sending is enabled, the device sends the highest threshold-crossed ARP packet rate within the sending interval in a notification to the SNMP module. You must use the snmp-agent target-host command to set the notification type and target host. For more information about notifications, see Network Management and Monitoring Command Reference.
·     If logging for ARP packet rate limit is enabled, the device sends the highest threshold-crossed ARP packet rate within the sending interval in a log message to the information center. You can configure the information center module to set the log output rules. For more information about information center, see Network Management and Monitoring Configuration Guide.
As a best practice, configure this feature when ARP attack detection or ARP snooping is enabled, or when ARP flood attacks are detected.
If excessive notifications and log messages are sent for ARP packet rate limit, you can increase notification and log message sending interval.
If you enable notification sending and logging for ARP packet rate limit on an aggregate interface, the features apply to all aggregation member ports.
The ARP packet rate limit configured in Ethernet interface view or aggregate interface view takes effect only on the current interface. The limit on an aggregation member port takes effect only when the member port leaves the aggregation group.
2.     (Optional.) Enable SNMP notifications for ARP packet rate limit.
snmp-agent trap enable arp [ rate-limit ]
By default, SNMP notifications for ARP packet rate limit are disabled.
3.     (Optional.) Enable logging for ARP packet rate limit.
arp rate-limit log enable
By default, logging for ARP packet rate limit is disabled.
4.     (Optional.) Set the notification and log message sending interval.
arp rate-limit log interval interval
By default, the device sends notifications and log messages every 60 seconds.
5.     Enter interface view.
Supported interface types include Layer 2 Ethernet interface and Layer 2 aggregate interface.
6.     Enable ARP packet rate limit.
arp rate-limit [ pps ]
By default, ARP packet rate limit is enabled, and the default rate limit is 500 pps.
This feature checks the number of ARP packets delivered to the CPU. If the number of packets from the same MAC address within 5 seconds exceeds a threshold, the device generates an ARP attack detection entry for the MAC address. If logging is enabled for source MAC-based ARP attack detection, the device handles the attack by using either of the following methods before the ARP attack detection entry ages out:
·     Monitor—Only generates log messages.
·     Filter—Generates log messages and filters out subsequent ARP packets from the MAC address.
When an ARP attack detection entry ages out, ARP packets sourced from the MAC address in the entry can be processed correctly.
When you change the handling method from monitor to filter, the configuration takes effect immediately. When you change the handling method from filter to monitor, the device continues filtering packets that match existing ARP attack detection entries, and uses the monitor method to process packets that match the new ARP attack detection entries.
Some gateways or important servers might send a large number of ARP packets, which is normal. To avoid dropping ARP packets from such devices, exclude the MAC addresses of those devices from source MAC-based ARP attack detection.
2.     Enable source MAC-based ARP attack detection and specify the handling method.
arp source-mac { filter | monitor }
3.     Set the threshold.
arp source-mac threshold threshold-value
By default, the threshold is 30.
4.     Set the aging timer for ARP attack detection entries.
arp source-mac aging-time time
By default, the lifetime is 300 seconds.
5.     (Optional.) Exclude specific MAC addresses from this detection.
arp source-mac exclude-mac mac-address&<1-10>
By default, no MAC address is excluded.
6.     Enable logging for source MAC-based ARP attack detection.
arp source-mac log enable
By default, logging for source MAC-based ARP attack detection is disabled.
Display ARP attack detection entries generated by source MAC-based ARP attack detection.
display arp source-mac { interface interface-type interface-number [ slot slot-number ] | slot slot-number }
As shown in Figure 2, the hosts access the Internet through a gateway (Device). If malicious users send a large number of ARP requests to the gateway, the gateway might crash and cannot process requests from the clients. To solve this problem, configure source MAC-based ARP attack detection on the gateway.
Figure 2  Network diagram
# Enable source MAC-based ARP attack detection, and specify the handling method as filter.
[Device] arp source-mac filter
# Set the threshold to 30.
[Device] arp source-mac threshold 30
# Set the lifetime for source MAC-based ARP attack detection entries to 60 seconds.
[Device] arp source-mac aging-time 60
# Exclude MAC address 0012-3f86-e94c from this detection.
[Device] arp source-mac exclude-mac 0012-3f86-e94c
This feature enables a gateway to filter ARP packets whose source MAC address in the Ethernet header is different from the sender MAC address in the message body. This feature allows the gateway to learn correct ARP entries.
2.     Enable ARP packet source MAC address consistency check.
arp valid-check enable
By default, ARP packet source MAC address consistency check is disabled.
Use the ARP active acknowledgement feature on gateways to prevent user spoofing.
This feature enables the device to perform active acknowledgement before creating an ARP entry.
·     Upon receiving an ARP request that requests the MAC address of the device, the device sends an ARP reply. Then, it sends an ARP request for the sender IP address in the received ARP request to determine whether to create an ARP entry for the sender IP address.
¡     If the device receives an ARP reply within the probe interval, it creates the ARP entry.
¡     If the device does not receive an ARP reply within the probe interval, it does not create the ARP entry.
·     Upon receiving an ARP reply, the device examines whether it was the reply to the request that the device has sent.
¡     If it was, the device creates an ARP entry for the sender IP address in the ARP reply.
¡     If it was not, the device sends an ARP request for the sender IP address to determine whether to create an ARP entry for the sender IP address.
-     If the device receives an ARP reply within the probe interval, it creates the ARP entry.
-     If the device does not receive an ARP reply within the probe interval, it does not create the ARP entry.
To improve validity and reliability of ARP entries, you can enable ARP active acknowledgement in strict mode. In this mode, the device creates ARP entries only for the IP addresses that the device actively initiates the ARP resolution.
2.     Enable ARP active acknowledgement.
arp active-ack [ strict ] enable
By default, ARP active acknowledgement is disabled.
For ARP active acknowledgement to take effect in strict mode, make sure ARP blackhole routing is enabled.
Authorized ARP entries are generated based on the DHCP clients' address leases on the DHCP server or dynamic client entries on the DHCP relay agent. For more information about DHCP server and DHCP relay agent, see Layer 3—IP Services Configuration Guide.
Use this feature to prevent user spoofing and to allow only authorized clients to access network resources.
2.     Enter interface view.
Only VLAN interfaces are supported.
3.     Enable authorized ARP on the interface.
arp authorized enable
By default, authorized ARP is disabled.
ARP attack detection enables access devices to block ARP packets from unauthorized clients to prevent user spoofing and gateway spoofing attacks.
ARP attack detection provides the following features:
·     User validity check.
·     ARP packet validity check.
·     ARP restricted forwarding.
·     ARP packet ingress port ignoring during user validity check
·     ARP attack detection logging.
If both ARP packet validity check and user validity check are enabled, the former one applies first, and then the latter applies.
Do not configure ARP attack detection together with ARP snooping. Otherwise, ARP snooping entries cannot be generated.
A Layer 2 Ethernet interface is enabled with ARP attack detection after you enable ARP attack detection on the interface or in the VLAN to which the interface belongs.
A Layer 2 Ethernet interface is disabled with ARP attack detection only after you disable ARP attack detection both on the interface and in the VLAN to which the interface belongs.
If a Layer 2 Ethernet interface is both enabled with ARP attack detection and configured as an ARP trusted port, the ARP trusted port configuration takes effect. The device does not perform ARP attack detection on packets received on the interface.
To prevent user spoofing, the device can perform user validity check on ARP packets. The interfaces that receive ARP packets are divided into the following types:
·     ARP trusted interface—The device does not perform user validity check on ARP packets. It directly forwards them.
·     ARP untrusted interface—The device performs user validity check on ARP packets.
This feature compares the sender IP and sender MAC in the received ARP packet with the matching criteria in the following order:
1.     User validity check rules.
¡     If a match is found, the device processes the ARP packet according to the rule.
¡     If no match is found, proceeds to the next step.
2.     IPSG bindings.
IPSG bindings include manually configured static IPSG bindings, and dynamic IPSG bindings automatically generated based on DHCP snooping and 802.1X.
User validity check that uses DHCP snooping-based dynamic IPSG bindings is typically called Dynamic ARP Inspection (DAI).
If a match is found, the device determines that the ARP packet is valid, and then forwards the ARP packet. During forwarding, it searches IPSG bindings for a match based on the destination IP address.
¡     If a match is found and the receiving interface is different from the interface in the entry with a matching sender IP address, the device performs Layer 3 forwarding.
¡     If a match is found but the receiving interface is the same as the interface in the entry with a matching sender IP address, the device performs Layer 2 forwarding.
¡     If no match is found, the device performs Layer 2 forwarding.
3.     If no matching rule or binding is found, the device discards the ARP packet.
Static IP source guard bindings are created by using the ip source binding command. For more information, see "Configuring IP source guard."
DHCP snooping-based dynamic IPSG bindings are automatically generated by DHCP snooping. For more information, see Layer 3—IP Services Configuration Guide.
802.1X-based dynamic IPSG bindings record the IP-to-MAC mappings for 802.1X clients. After a client passes 802.1X authentication and uploads its IP address to an ARP attack detection enabled device, the device automatically generates an 802.1X security entry. The 802.1X client must be enabled to upload its IP address to the device. For more information, see "Configuring 802.1X."
When you configure user validity check, make sure one or more of the following items are configured:
·     User validity check rules.
·     Static IP source guard bindings.
·     DHCP snooping.
·     802.1X.
If none of the items is configured, no incoming ARP packets on ARP untrusted interfaces can be forwarded normally.
Specify an IP address, a MAC address, and a VLAN where ARP attack detection is enabled for an IP source guard binding. Otherwise, no ARP packets can match the IP source guard binding.
Configuring user validity check rules
2.     Configure a user validity check rule.
arp detection rule rule-id { deny | permit } ip { ip-address [ mask ] | any } mac { mac-address [ mask ] | any } [ vlan vlan-id ]
By default, no user validity check rules are configured.
Enabling ARP attack detection in a VLAN
2.     Enter VLAN view.
vlan vlan-id
3.     Enable ARP attack detection.
arp detection enable
By default, ARP attack detection is disabled. The device does not perform ARP user validity check.
4.     (Optional.) Configure an interface that does not require ARP user validity check as a trusted interface.
a.     Return to system view.
b.     Enter interface view.
c.     Configure the interface as a trusted interface excluded from ARP attack detection.
arp detection trust
By default, an interface is untrusted.
Enabling ARP attack detection on a Layer 2 interface
Supported interfaces include Layer 2 Ethernet interfaces and Layer 2 aggregate interfaces.
By default, ARP attack detection is disabled. The device does not perform user validity check.
ARP packet validity check does not check ARP packets received on ARP trusted interfaces. To check ARP packets received on untrusted interfaces, you can specify the following objects to be checked:
·     src-mac—Checks whether the sender MAC address in the message body is identical to the source MAC address in the Ethernet header. If they are identical, the packet is forwarded. Otherwise, the packet is discarded.
·     dst-mac—Checks the target MAC address of ARP replies. If the target MAC address is all-zero, all-one, or inconsistent with the destination MAC address in the Ethernet header, the packet is considered invalid and discarded.
·     ip—Checks the sender and target IP addresses of ARP replies, and the sender IP address of ARP requests. All-one or multicast IP addresses are considered invalid and the corresponding packets are discarded.
Before you configure ARP packet validity check, you must first configure user validity check. For more information about user validity check configuration, see "Configuring user validity check."
Enabling ARP packet validity check
2.     Enter VLAN view.
vlan vlan-id
By default, ARP attack detection is disabled. The device does not perform ARP packet validity check.
4.     Enable ARP packet validity check.
b.     Enable ARP packet validity check and specify the objects to be checked.
By default, ARP packet validity check is disabled.
2.     Enter VLAN view.
vlan vlan-id
4.     (Optional.) Configure the interface that does not require ARP packet validity check as a trusted interface.
arp detection trust
ARP restricted forwarding does not take effect on ARP packets received on ARP trusted interfaces and forwards the ARP packets correctly. This feature controls the forwarding of ARP packets that are received on untrusted interfaces and have passed user validity check as follows:
·     If the packets are ARP requests, they are forwarded through the trusted interface.
·     If the packets are ARP replies, they are forwarded according to their destination MAC address. If no match is found in the MAC address table, they are forwarded through the trusted interface.
ARP restricted forwarding does not apply to ARP packets that use multiport destination MAC addresses.
Configure user validity check before you configure ARP restricted forwarding. For information about user validity check configuration, see "Configuring user validity check."
2.     Enter VLAN view.
vlan vlan-id
3.     Enable ARP restricted forwarding.
By default, ARP restricted forwarding is disabled.
ARP attack detection performs user validity check on ARP packets from ARP untrusted interfaces. The sender IP and sender MAC in the received ARP packet are compared with the entries used for user validity check. In addition, user validity check compares the ingress port of the ARP packet with the port in the entries. If no matching port is found, the ARP packet is discarded. For more information about user validity check, see "Configuring user validity check."
You can configure the device to ignore the ingress ports of ARP packets during user validity check. If an ARP packet passes user validity check, the device directly performs Layer 2 forwarding for the packet. It no longer searches for a matching static IPSG binding, 802.1X security entry, or DHCP snooping entry by the target IP address of the ARP packet.
2.     Ignore ingress ports of ARP packets during user validity check.
arp detection port-match-ignore
By default, ingress ports of ARP packets are checked during user invalidity.
The ARP attack detection logging feature enables a device to generate ARP attack detection log messages when illegal ARP packets are detected. An ARP attack detection log message contains the following information:
·     Receiving interface of the ARP packets.
·     Sender IP address.
·     Total number of dropped ARP packets.
2.     Enable ARP attack detection logging.
arp detection log enable [ interval interval | number number | threshold threshold-value ]*
By default, ARP attack detection logging is disabled.
Display the VLANs and interfaces enabled with ARP attack detection.
display arp detection
Display ARP attack source statistics.
display arp detection statistics attack-source slot slot-number
Display statistics for packets dropped by ARP attack detection.
display arp detection statistics packet-drop [ interface interface-type interface-number ]
Clear ARP attack source statistics.
reset arp detection statistics attack-source [ slot slot-number ]
Clear statistics for packets dropped by ARP attack detection.
reset arp detection statistics packet-drop [ interface interface-type interface-number ]
As shown in Figure 3, configure Device B to perform user validity check based on 802.1X security entries for connected hosts.
Figure 3 Network diagram
1.     Add all interfaces on Device B to VLAN 10, and specify the IP address of VLAN-interface 10 on Device A. (Details not shown.)
2.     Configure the DHCP server on Device A, and configure DHCP address pool 0.
[DeviceA] dhcp enable
[DeviceA] dhcp server ip-pool 0
[DeviceA-dhcp-pool-0] network 10.1.1.0 mask 255.255.255.0
3.     Configure Host A and Host B as 802.1X clients and configure them to upload IP addresses for ARP attack detection. (Details not shown.)
4.     Configure Device B:
# Enable 802.1X.
[DeviceB] dot1x
[DeviceB-GigabitEthernet1/0/1] dot1x
[DeviceB-GigabitEthernet1/0/2] dot1x
# Add a local user test.
[DeviceB] local-user test class network
[DeviceB-luser-network-test] service-type lan-access
[DeviceB-luser-network-test] password simple test
[DeviceB-luser-network-test] quit
# Enable ARP attack detection for VLAN 10 to check user validity based on 802.1X entries.
[DeviceB] vlan 10
[DeviceB-vlan10] arp detection enable
# Configure the upstream interface as an ARP trusted interface. By default, an interface is an untrusted interface.
[DeviceB-vlan10] interface gigabitethernet 1/0/3
[DeviceB-GigabitEthernet1/0/3] arp detection trust
# Verify that ARP packets received on interfaces GigabitEthernet 1/0/1 and GigabitEthernet 1/0/2 are checked against 802.1X entries.
As shown in Figure 4, configure Device B to perform ARP packet validity check and user validity check based on static IP source guard bindings and DHCP snooping entries for connected hosts.
Figure 4 Network diagram
3.     Configure Host A (DHCP client) and Host B. (Details not shown.)
# Enable DHCP snooping.
[DeviceB] dhcp snooping enable
[DeviceB] interface gigabitethernet 1/0/3
[DeviceB-GigabitEthernet1/0/3] dhcp snooping trust
# Enable recording of client information in DHCP snooping entries on GigabitEthernet 1/0/1.
[DeviceB-GigabitEthernet1/0/1] dhcp snooping binding record
# Enable ARP attack detection for VLAN 10.
[DeviceB] vlan 10
# Configure the upstream interface as a trusted interface. By default, an interface is an untrusted interface.
# Configure a static IP source guard binding entry on interface GigabitEthernet 1/0/2 for user validity check.
[DeviceB-GigabitEthernet1/0/2] ip source binding ip-address 10.1.1.6 mac-address 0001-0203-0607 vlan 10
# Enable ARP packet validity check by checking the MAC addresses and IP addresses of ARP packets.
[DeviceB] arp detection validate dst-mac ip src-mac
# Verify that Device B first checks the validity of ARP packets received on GigabitEthernet 1/0/1 and GigabitEthernet 1/0/2. If the ARP packets are confirmed valid, Device B performs user validity check by using the static IP source guard bindings and finally DHCP snooping entries.
As shown in Figure 5, configure ARP restricted forwarding on Device B where ARP attack detection is configured. Port isolation configured on Device B can take effect for broadcast ARP requests.
Figure 5 Network diagram
1.     Configure VLAN 10, add interfaces to VLAN 10, and specify the IP address of VLAN-interface 10 on Device A. (Details not shown.)
# Enable DHCP snooping, and configure GigabitEthernet 1/0/3 as a DHCP trusted interface.
# Enable ARP attack detection for user validity check.
[DeviceB] vlan 10
# Configure GigabitEthernet 1/0/3 as an ARP trusted interface.
# Configure a static IP source guard entry on interface GigabitEthernet 1/0/2.
# Configure port isolation.
[DeviceB] port-isolate group 1
[DeviceB-GigabitEthernet1/0/1] port-isolate enable group 1
[DeviceB-GigabitEthernet1/0/2] port-isolate enable group 1
After the configurations are completed, Device B first checks the validity of ARP packets received on GigabitEthernet 1/0/1 and GigabitEthernet 1/0/2. If the ARP packets are confirmed valid, Device B performs user validity check by using the static IP source guard bindings and finally DHCP snooping entries. However, ARP broadcast requests sent from Host A can pass the check on Device B and reach Host B. Port isolation fails.
# Enable ARP restricted forwarding.
[DeviceB] vlan 10
[DeviceB-vlan10] arp restricted-forwarding enable
[DeviceB-vlan10] quit
# Verify that Device B forwards ARP broadcast requests from Host A to Device A through the trusted interface GigabitEthernet 1/0/3. Host B cannot receive such packets. Port isolation operates correctly.
ARP scanning is typically used together with the fixed ARP feature in small-scale and stable networks.
ARP scanning automatically creates ARP entries for devices in an address range. The device performs ARP scanning in the following steps:
1.     Sends ARP requests for each IP address in the address range.
2.     Obtains their MAC addresses through received ARP replies.
3.     Creates dynamic ARP entries.
You can manually trigger ARP scanning or enable automatic ARP scanning. Automatic ARP scanning periodically sends ARP requests for all IP addresses in the range at the specified rate set by using the arp scan auto send-rate command.
Fixed ARP converts existing dynamic ARP entries (including those generated through ARP scanning) to static ARP entries. These static ARP entries are of the same attributes as the ARP entries that are manually configured. This feature prevents ARP entries from being modified by attackers.
You can set the ARP packet sending rate if the scanning range has a large number of IP addresses. This setting can avoid high CPU usage and heavy network load caused by a burst of ARP traffic.
IP addresses in existing ARP entries are not scanned.
If you trigger ARP scanning and enable automatic ARP scanning, both of them take effect. As a best practice, use automatic ARP scanning only on networks where users come online and go offline frequently.
Due to the limit on the total number of static ARP entries, some dynamic ARP entries might fail the conversion.
The arp fixup command is a one-time operation. You can use this command again to convert the dynamic ARP entries learned later to static.
To delete a static ARP entry converted from a dynamic one, use the undo arp ip-address [ vpn-instance-name ] command. You can also use the reset arp all command to delete all ARP entries or the reset arp static command to delete all static ARP entries.
3.     Trigger ARP scanning.
arp scan [ start-ip-address to end-ip-address ] [ send-rate { ppm ppm | pps } ]
CAUTION
CAUTION:
ARP scanning will take some time and occupy a lot of system and network resources. To stop an ongoing scan, press Ctrl + C. Dynamic ARP entries are created based on ARP replies received before the scan is terminated.
2.     Set the ARP packet sending rate for automatic ARP scanning.
arp scan auto send-rate { ppm ppm | pps pps }
By default, the device sends ARP packets at the rate of 48 pps during automatic ARP scanning.
3.     Enter interface view.
4.     Enable automatic ARP scanning.
arp scan auto enable [start-ip-address to end-ip-address ]
By default, automatic ARP scanning is disabled.
2.     Convert existing dynamic ARP entries to static ARP entries.
arp fixup
In a large-scale network, it takes a long time for ARP scanning to identify the hosts that go offline abnormally if you specify a large scanning range. After you enable ARP keepalive entry scanning, the system can quickly locate those hosts and monitor the host status within the aging time.
You can set the aging time for ARP keepalive entries in both system view and interface view. The aging time set in interface view takes precedence over the aging time set in system view. In interface view, the default aging time for ARP keepalive entries is the aging time set in system view.
When users come online, the system generates dynamic APR entries and IPSG binding entries. Enabled with ARP keepalive entry scanning, the system also creates online keepalive entries when users come online. If users go offline, the corresponding APR entries are deleted and the status of the keepalive entries is set to offline. The device sends ARP requests at intervals to the IP addresses in the offline keepalive entries until the keepalive entries become online again or are deleted when the aging time expires. The interval varies with the number of ARP requests that have been sent to the IP address in an offline keepalive entry. For more information about IP source guard configuration, see Security Configuration Guide.
2.     (Optional.) Set the ARP request sending rate for keepalive entry scanning.
arp scan keepalive send-rate pps
By default, the device sends ARP requests at a rate of 48 pps during keepalive entry scanning.
3.     (Optional.) Set the aging time for ARP keepalive entries.
arp scan keepalive aging-time time
By default, the aging time for ARP keepalive entries in system view is 60 minutes. The aging time for ARP keepalive entries in interface view is the aging time set in system view.
4.     Enter interface view.
5.     Enable the ARP keepalive entry scanning feature.
arp scan keepalive enable
By default, the ARP keepalive entry scanning is disabled on an interface.
Display ARP keepalive entries.
display arp scan keepalive entry [ interface interface-type interface-number ] [ count ]
Display statistics about ARP requests sent to the IP addresses in offline keepalive entries for an interface.
display arp scan keepalive statistics [ slot slot-number ] [ interface interface-type interface-number ]
Clear statistics about ARP requests sent to the IP addresses in offline keepalive entries.
reset arp scan keepalive statistics [ slot slot-number ]
Configure this feature on interfaces not connected with a gateway to prevent gateway spoofing attacks.
When such an interface receives an ARP packet, it checks whether the sender IP address in the packet is consistent with that of any protected gateway. If yes, it discards the packet. If not, it handles the packet correctly.
You can enable ARP gateway protection for a maximum of eight gateways on an interface.
Do not configure both the arp filter source and arp filter binding commands on an interface.
If ARP gateway protection works with ARP attack detection and ARP snooping, ARP gateway protection applies first.
3.     Enable ARP gateway protection for the specified gateway.
arp filter source ip-address
By default, ARP gateway protection is disabled.
As shown in Figure 6, Host B launches gateway spoofing attacks to Device B. As a result, traffic that Device B intends to send to Device A is sent to Host B.
Configure Device B to block such attacks.
Figure 6 Network diagram
# Configure ARP gateway protection on Device B.
[DeviceB-GigabitEthernet1/0/1] arp filter source 10.1.1.1
[DeviceB-GigabitEthernet1/0/2] arp filter source 10.1.1.1
# Verify that GigabitEthernet 1/0/1 and GigabitEthernet 1/0/2 discard the incoming ARP packets whose sender IP address is the IP address of the gateway.
About ARP filtering
The ARP filtering feature can prevent gateway spoofing and user spoofing attacks.
An interface enabled with this feature checks the sender IP and MAC addresses in a received ARP packet against permitted entries. If a match is found, the packet is handled correctly. If not, the packet is discarded.
You can configure a maximum of eight permitted entries on an interface.
If ARP filtering works with ARP attack detection and ARP snooping, ARP filtering applies first.
Supported interface types include Ethernet interface and Layer 2 aggregate interface.
3.     Enable ARP filtering and configure a permitted entry.
By default, ARP filtering is disabled.
As shown in Figure 7, the IP and MAC addresses of Host A are 10.1.1.2 and 000f-e349-1233, respectively. The IP and MAC addresses of Host B are 10.1.1.3 and 000f-e349-1234, respectively.
Configure ARP filtering on GigabitEthernet 1/0/1 and GigabitEthernet 1/0/2 of Device B to permit ARP packets from only Host A and Host B.
Figure 7 Network diagram
# Configure ARP filtering on Device B.
[DeviceB-GigabitEthernet1/0/1] arp filter binding 10.1.1.2 000f-e349-1233
[DeviceB-GigabitEthernet1/0/2] arp filter binding 10.1.1.3 000f-e349-1234
# Verify that GigabitEthernet 1/0/1 permits ARP packets from Host A and discards other ARP packets.
# Verify that GigabitEthernet 1/0/2 permits ARP packets from Host B and discards other ARP packets.
This feature allows a gateway to check the sender IP address of an ARP packet in a VLAN before ARP learning. If the sender IP address is within the allowed IP address range, the gateway continues ARP learning. If the sender IP address is out of the range, the gateway determines the ARP packet as an attack packet and discards it.
2.     Enter VLAN view.
vlan vlan-id
3.     Enable the ARP sender IP address checking feature and specify the IP address range.
arp sender-ip-range start-ip-address end-ip-address
By default, the ARP sender IP address checking feature is disabled.
Enable SNMP notifications for ARP as required.
·     If you enable ARP active acknowledgement notifications, the device sends a notification to the SNMP module when it does not establish an ARP entry due to active acknowledgement. The notification includes the sender IP address in the received ARP packet and the interface that receives the ARP packet.
·     If you enable rate limit notifications for sending ARP Miss messages and ARP packets, the device sends the highest threshold-crossed rate as a notification to the SNMP module when the sending rate exceeds the custom threshold.
·     If you enable notifications for packet dropping due to ARP attack detection, the device sends a notification to the SNMP module when a packet is dropped by ARP attack detection. The notification includes the VLAN ID and drop reason for the dropped packet.
·     If you enable ARP entry modification notifications, the device sends a notification to the SNMP module when it detects that the ARP entry for a user might be changed to the attacker's ARP entry. The notification includes the sender IP and MAC addresses in the ARP attack packet.
·     If you enable ARP entry limit notifications, the device sends the current number of ARP entries as a notification to the SNMP module when the number of global ARP entries exceeds the alarm threshold.
·     If you enable ARP gateway protection notifications, the device sends a notification to the SNMP module when it is attacked by gateway spoofing attacks. The notification includes the sender IP and MAC addresses in the ARP attack packet dropped by ARP gateway protection, and index of the interface that receives the ARP attack packet. When an ARP packet with the same sender IP address triggers the SNMP notification again within 3 minutes, the device sends a recovery notification to the SNMP module.
·     If you enable endpoint and local device conflict notifications, the device sends a notification to the SNMP module when an endpoint and local device conflict occurs. The notification includes the sender IP address, sender MAC address, target IP address, and target MAC address in the conflicting ARP packet.
·     If you enable MAC address inconsistency notifications, the device sends a notification to the SNMP module when the MAC address in the configured static ARP entry and user's actual MAC address are inconsistent. The notification includes the IP address, VPN instance, and MAC address in the ARP entry.
·     An invalid ARP packet contains an invalid hardware address type, protocol address type, hardware address length, protocol address length, operation code, or VLAN. For example, when the operation code value is not 1 (ARP request) or 2 (ARP reply), the operation code is invalid and the ARP packet is invalid. If you enable invalid ARP packet check notifications, the device sends a notification to the SNMP module when it receives an invalid ARP packet. The notification includes the name of the interface that receives the ARP packet, sender MAC and IP addresses, user VLAN ID, and VLAN ID of the service provider.
·     If you enable ARP packet queue limit notifications, the device sends the number of packets in the queue as a notification to the SNMP module when the number exceeds 80% of the upper limit.
·     If you enable rate limit notifications for receiving ARP packets, the device sends the highest threshold-crossed rate as a notification to the SNMP module. For more information about ARP packet rate limit, see "Configuring ARP packet rate limit."
·     If you enable user IP address conflict notifications, the device sends a notification to the SNMP module when a user IP address conflict occurs. The notification includes the sender IP and MAC addresses in the conflicting ARP packet, and MAC address in the corresponding local ARP entry. For more information about enabling recording user IP address conflicts, see ARP configuration in Layer 3—IP Services Configuration Guide.
·     If you enable user port migration notifications, the device sends a notification to the SNMP module when a user port changes. The notification includes the IP address, MAC address, port before migration, and port after migration of the user. For more information about enabling recording user port migrations, see ARP configuration in Layer 3—IP Services Configuration Guide.
For ARP event notifications to be sent correctly, you must also configure SNMP on the device. For more information about SNMP configuration, see Network Management and Monitoring Configuration Guide.
2.     Enable SNMP notifications for ARP.
snmp-agent trap enable arp [ active-ack | arp-miss | detection-drop | entry-check | entry-limit | gateway-check | local-conflict | mac-mismatch | packet-check | pkt-threshold | rate-limit | user-ip-conflict | user-move ] *
By default, SNMP notifications for ARP are disabled.
If you do not specify any keywords, this command enables all SNMP notifications for ARP.