| 06-PoE Issues | 66.76 KB |
PoE failures
PoE power supply failure
PoE power supply exception
Symptom
PoE power supply is insufficient or the PSE cannot supply power.
Common causes
· The power source does not match the device or has insufficient power.
· PSE firmware failure.
· The PD is a non standard PD and nonstandard PD detection is not enabled.
Troubleshooting flow
Figure 1 shows the troubleshooting flowchart.
Solution
1. Verify that correct power supplies are installed on the device.
For a PoE switch, use power supplies according to the PoE power supply scheme. For information about the power supply compatibility, see the installation guide for your device.
2. Identify whether PSE firmware is operating correctly.
Execute the display poe device command to display PSE information. If the state is faulty, the PSE has issues.
<Sysname> display poe device
Slot 1:
PSE ID Slot No. SSlot No. PortNum MaxPower(W) State Model
1 0 0 48 0 Faulty LSP1POEA
The output shows that the PSE has issues.
Contact Technical Support or the device vendor to obtain the PSE firmware of the target version, and then execute the poe update command to upgrade the PSE processing software in service.
[Sysname] poe update full POE-168.bin pse 4
This command will refresh the PSE firmware. Continue? [Y/N]:y
The output shows that the PSE processing software has been upgraded. Execute the display poe device command again to display PSE information, and check the on or off field for the PSE state.
[Sysname] display poe device
Slot 1:
1 0 0 48 0 on LSP1POEA
3. Execute the display poe pse command in any view to display detailed PSE information. Verify the following information:
¡ The current power, average power, and peak power of the PSE are correct.
¡ Nonstandard PD detection by the PSE is enabled.
<Sysname> display poe pse
PSE ID : 1
Slot NO. : 0
PSE Model : LSBMPOEGV48TP
PSE Status : Enabled
PSE Preempted : No
Power Priority : Low
Current Power : 130 W
Average Power : 20 W
Peak Power : 240 W
Max Power : 200 W
Remaining Guaranteed Power : 120 W
PSE CPLD Version : 100
PSE Software Version : 200
PSE Hardware Version : 100
Legacy PD Detection : Disabled
Power Utilization Threshold : 80
PSE Power Policy : Disabled
PD Power Policy : Disabled
PD Disconnect-Detection Mode : DC
¡ If the current power, average power, and peak power of the PSE are close to or reach the maximum power of the PSE, use PoE power with higher-wattage supply.
¡ If the PSE Legacy PD Detection field displays Disable, execute the poe legacy enable command to enable nonstandard PD detection.
4. Execute the display poe interface command in any view to display power supply information. Verify the following information:
¡ The PoE interface current and voltage are correct.
<Sysname> display poe interface gigabitethernet 1/0/1
PoE Status : Enabled
Power Priority : Critical
Oper : On
IEEE Class : 1
Detection Status : Delivering power
Power Mode : Signal
Current Power : 11592 mW
Average Power : 11610 mW
Peak Power : 11684 mW
Max Power : 15400 mW
Electric Current : 244 mA
Voltage : 51.7 V
PD Description : IP Phone For Room 101
If the current power, average power, and peak power of the PoE interface are close to or reach the maximum power of the PoE interface, execute the poe max-power command to configure the maximum power.
5. If the issue persists, collect the information and contact Technical Support.