11-Network Management and Monitoring Configuration Guide
HomeSupportConfigure & DeployConfiguration GuidesH3C S5560S-EI[SI]&S5500V3-SI&MS4520V2&WS5850-Winet Configuration Guides-R63xx-6W10411-Network Management and Monitoring Configuration Guide
04-PoE configuration
04-PoE configuration 266.67 KB
Configuring PoE
About PoE
Power over Ethernet (PoE) enables a network device to supply power to terminals over twisted pair cables.
PoE system
As shown in Figure 1, a PoE system includes the following elements:
·     PoE power supply—A PoE power supply provides power for the entire PoE system.
·     PSE—A power sourcing equipment (PSE) supplies power to PDs. PSE devices are classified into single-PSE devices and multiple-PSE devices.
¡     A single-PSE device has only one PSE firmware.
¡     A multiple-PSE device has multiple PSEs. A multiple-PSE device uses PSE IDs to identify different PSEs. To view the mapping between the ID and slot number of a PSE, execute the display poe device command.
·     PI—A power interface (PI) is a PoE-capable Ethernet interface on a PSE.
·     PD—A powered device (PD) receives power from a PSE. PDs include IP telephones, APs, portable chargers, POS terminals, and Web cameras. You can also connect a PD to a redundant power source for reliability.
Figure 1 PoE system diagram
AI-driven PoE
AI-driven PoE innovatively integrates AI technologies into PoE switches and offers the following benefits:
·     Adaptive power supply management
AI-driven PoE can adaptively adjust the power supply parameters to fit power needs in various scenarios such as multiple types of PDs and address issues such as no power supply to a PD and power failure, minimizing human intervention.
·     Priority-based power management
When the power demanded by PDs exceeds the power that can be supplied by the PoE switch, the system supplies power to PDs based on the PI priorities to ensure power supply to critical businesses and reduce power supply to PIs of lower priorities.
·     Smart power module management
For a PoE switch with a dual power module architecture, AI-driven PoE can automatically calculate and regulate power output of each power module based on the type and quantity of the power modules, maximizing the power usage of each power module. When a power module is removed, AI-driven PoE recalculates to preferentially guarantee power supply to PDs that are being powered.
·     High PoE security
When an exception such as short circuit or circuit break occurs, AI-driven PoE immediately starts self-protection to protect the PoE switch from being damaged or burned.
·     Perpetual PoE
During a hot reboot of the PoE switch from the reboot command, AI-driven PoE continuously monitors the PD states and ensures continued power supply to PDs, maintaining terminal service stability.
·     Remote PoE
AI-driven PoE adaptively adjusts the network bandwidth based on the transmission distance between a PSE and PD. When the transmission distance exceeds 100 m (328.08 ft), the system automatically decreases the port rate to reduce the line loss and ensure the signal and power transmission quality. With AI-driven PoE enabled, a PSE can transmit power to a PD of 200 to 250 m (656.17 to 820.21 ft) away.
Protocols and standards
·     802.3af-2003, IEEE Standard for Information Technology - Telecommunications and Information Exchange Between Systems - Local and Metropolitan Area Networks - Specific Requirements - Part 3: Carrier Sense Multiple Access with Collision Detection (CSMA/CD) Access Method and Physical Layer Specifications - Data Terminal Equipment (DTE) Power Via Media Dependent Interface (MDI)
·     802.3at-2009, IEEE Standard for Information technology-- Local and metropolitan area networks-- Specific requirements-- Part 3: CSMA/CD Access Method and Physical Layer Specifications Amendment 3: Data Terminal Equipment (DTE) Power via the Media Dependent Interface (MDI) Enhancements
Restrictions: Hardware compatibility with PoE
Only the PoE models support the PoE feature.
Restrictions and guidelines: PoE configuration
You can configure a PI through either of the following ways:
·     Configure the settings directly on the PI.
·     Configure a PoE profile and apply it to the PI. If you apply a PoE profile to multiple PIs, these PIs have the same PoE features. If you connect a PD to another PI, you can apply the PoE profile of the original PI to the new PI. This method relieves the task of configuring PoE on the new PI.
You can only use one way to configure a parameter for a PI. To use the other way to reconfigure a parameter, you must first remove the original configuration.
You must use the same configuration method for the poe max-power max-power and poe priority { critical | high | low } commands.
PoE configuration tasks at a glance
To configure PoE, perform the following tasks:
1.     Enabling PoE on a PI
2.     (Optional.) Enabling AI-driven PoE
3.     (Optional.) Enabling fast PoE for a PSE
4.     (Optional.) Configuring PoE delay
5.     (Optional.) Disabling PoE power supply on shutdown interfaces
6.     (Optional.) Allowing inrush currents drawn by PDs
7.     (Optional.) Enabling PI power cycling upon a system warm reboot
8.     (Optional.) Ignoring the PD power class
9.     (Optional.) Configuring PD detection
¡     Enabling nonstandard PD detection
¡     Configuring a PD detection mode
¡     Configuring a PD disconnection detection mode
10.     (Optional.) Configuring PoE power
¡     Configuring the maximum PI power
¡     Setting the PoE guard band
11.     (Optional.) Configuring the PI priority policy
12.     (Optional.) Configuring PSE power monitoring
13.     (Optional.) Upgrading PSE firmware in service
14.     (Optional.) Enabling forced PoE power supply
15.     (Optional.) Configuring the TMPDO for the MPS
To use a PoE profile to enable PoE and configure the priority, power transmission mode, and maximum power for a PI, see "Configuring a PI by using a PoE profile"
Prerequisites for configuring PoE
Before you configure PoE, make sure the PoE power supply and PSEs are operating correctly.
About enabling PoE on a PI
After you enable PoE on a PI, the PI supplies power to the connected PD if the PI will not result in PSE power overload. PSE overload occurs when the sum of the power consumption of all PIs exceeds the maximum power of the PSE.
If the PI will result in PSE power overload, the following restrictions apply:
·     If the PI priority policy is not enabled, the PI does not supply power to the connected PD.
·     If the PI priority policy is enabled, whether the PDs can be powered depends on the priority of the PI.
For more information about the PI priority policy, see "Configuring the PI priority policy."
Power can be transmitted over a twisted pair cable in either of the following modes:
·     Signal pair mode—Signal pairs 1, 2, 3, and 6 of the twisted pair cable are used for power transmission.
·     Spare pair mode—Spare pairs 4, 5, 7, and 8 of the twisted pair cable are used for power transmission.
A PI can supply power to a PD only when the PI and PD use the same power transmission mode. If the PI and PD use different power transmission modes, a reconnection is required.
The device supports power transmission only over signal pairs.
2.     Enter PI view.
3.     (Optional.) Configure a description for the PD connected to the PI.
poe pd-description text
By default, no description is configured for the PD connected to the PI.
4.     Enable PoE on the PI.
poe enable
¡     S5560S-EI switch series:
-     In Release 6328 or earlier, PoE is disabled on PIs by default.
-     In Release 6328 or later, PoE is enabled on PIs when the switch starts up with factory defaults and is disabled on PIs when the switch starts up with the initial configuration.
¡     WS5850-WiNet switch series: PoE is enabled on PIs when the switch starts up with factory defaults and is disabled on PIs when the switch starts up with the initial configuration.
For more information about the device initial configuration and factory defaults, see configuration file management in Fundamentals Configuration Guide.
AI-driven PoE takes effect only on PSEs that run firmware V147 or later.
·     Firmware earlier than V147—You must use the poe update command to upgrade the PSE firmware and then enable AI-driven PoE on the PSE.
·     Firmware V147 or later—You do not need to re-enable AI-driven PoE after upgrading the firmware if you have enabled the feature before the upgrade.
This feature is supported only in Release 6318P01 and later.
2.     Enable AI-driven PoE.
poe ai enable
By default, AI-driven PoE is disabled.
AI-driven PoE automatically adjusts the power supply parameters to fit the power needs. If you disable AI-driven PoE, the system reverts the parameters to the settings before the adjustment.
About fast PoE for a PSE
This feature enables a PI on a PSE to supply power to PDs immediately after the PSE is powered on.
You must re-configure this feature if you modified other PoE settings after configuring this feature.
2.     Enable fast PoE for a PSE.
poe fast-on enable pse pse-id
By default, fast PoE is disabled on a PSE.
This command is available only in Release 6328 and later.
By default, the device executes the poe enable command and supplies power to an interface immediately when any one of the following conditions is met:
·     The poe enable command is configured.
·     The device reboots with the poe enable command in the configuration file.
·     The interface comes up and the PoE module resumes PoE power supply to the interface.
This task creates a PoE delay timer after the poe enable command is executed and allows the PoE module to supply power to the PI only after the timer expires.
Software version and feature compatibility
This feature is supported only in Release 6351 and later.
The undo poe enable command is executed immediately upon configuration and is not affected by this feature.
2.     Enable PoE delay.
poe power-delay time
By default, PoE delay is disabled.
By default, the device continues supplying power to an interface after the interface is shut down by the shutdown command or by an upper layer module such as monitor link. As a result, the PD connected to the shutdown interface operates continuously but fails to access the network.
This task disables the PoE module from supplying power to an interface after the interface is shut down. After the interface comes up, the PoE module resumes power supply to the interface.
The command does not power off an interface that has been shut down but is supplying power to a PD.
2.     Disable PoE power supply on shutdown interfaces.
poe track-shutdown
About allowing inrush currents drawn by PDs
Inrush current might occur at PD startup and trigger PSE self-protection, As a result, the PSE stops supplying power to the PDs. To continue power supply to the PDs, configure this feature to allow inrush currents drawn by PDs.
IEEE 802.3af and IEEE 802.3at define specifications for inrush current. Support for the specifications defined by IEEE 802.3af and/or IEEE 802.3at depends on the device model.
CAUTION
CAUTION:
Inrush currents might damage the components on the device. Use this feature with caution.
This feature is available only for a PSE that has a model name ending with a character of B, LSPPSE48B for example. To obtain the PSE model name, execute the display poe pse command.
·     In versions earlier than Release 6351:
a.     Enter system view.
b.     Allow inrush currents drawn by PDs.
poe high-inrush enable pse pse-id
By default, inrush currents drawn by PDs are not allowed.
·     In Release 6351 and later:
b.     Enter PI view.
c.     Allow inrush currents drawn by PDs.
About enabling PI power cycling upon a system warm reboot
During the system warm reboot process (upon execution of the reboot command), the PIs continue supplying power to the PDs but data connections between the PDs and the device are interrupted. After the system reboots, PDs might not re-initiate data connections with the device. Power cycling PIs upon a system warm reboot allows the PDs to re-establish data connections with the device after a warm reboot.
2.     Enter PI power cycling upon a system warm reboot.
poe reset enable
By default, PI power cycling upon a system warm reboot is disabled.
Before supplying power to a PD, the device detects the power class of the PD by default. For example, if the device detects the power class of a PD as 1, the device can provide a maximum power of 12.95 W to the PD. If the power required by a PD is greater than 12.95 W, the device will stop supplying power to the PD.
After configuring this task, the device will continue to detect the PD power class before supplying power to a PD, but it will no limit the power supplied to the PD based on the detected power class. As long as the power required by the PD does not exceed the maximum power on the interface (configured by using the poe max power command in interface view), the device can supply power to the PD.
If you execute the poe class-detect ignore command multiple times, and the most recent configuration will take effect.
2.     Enter PI view.
3.     Ignore the PD power class.
By default, the device supplies power to PDs based on the detected PD power class.
About enabling nonstandard PD detection
PDs are classified into standard PDs and nonstandard PDs. Standard PDs are compliant with IEEE 802.3af and IEEE 802.3at. A PSE supplies power to a nonstandard PD only after nonstandard PD detection is enabled.
The device supports PSE-based and PI-based nonstandard PD detection. Enabling nonstandard PD detection for a PSE enables this feature for all PIs on the PSE. As a best practice for disabling nonstandard PD detection for all PIs successfully in one operation, disable this feature in both system view and interface view.
2.     Enable nonstandard PD detection. Choose one option as needed.
¡     Enable nonstandard PD detection for the PSE.
poe legacy enable pse pse-id
By default, nonstandard PD detection is disabled for a PSE.
¡     Execute the following commands in sequence to enable nonstandard PD detection for a PI:
poe legacy enable
By default, nonstandard PD detection is disabled for a PI.
About PD detection modes
The device detects PDs in one of the following modes:
·     None—The device supplies power to PDs that are correctly connected to the device without causing short circuit.
·     Simple—The device supplies power to PDs that comply with basic requirements of 802.3af or 802.3at.
·     Strict—The device supplies power to PDs that comply with all requirements of 802.3af or 802.3at.
CAUTION
CAUTION:
A non-PD device might be damaged when power is supplied to it. To avoid device damage, do not use the none mode when the PI connects to a non-PD device.
This task is available only for a PSE that has a model name ending with a character of B, LSPPSE48B for example. To obtain the PSE model name, execute the display poe pse command.
For this task to take effect on nonstandard PDs, you must enable detection for nonstandard PDs by using the poe legacy enable command.
2.     Enter PI view.
3.     Configure the PD detection mode.
poe detection-mode { none | simple | strict }
The default differs depending on the software version, as shown below:
Versions
Default setting
Versions earlier than Release 6351
The PD detection mode is strict.
·     If the device starts up with the initial configuration, the PD detection mode is strict.
·     If the device starts up with the factory defaults, the PD detection mode is simple.
CAUTION
CAUTION:
If you change the PD disconnection detection mode when the device is running, the connected PDs might be powered off. Be aware of the impact of this operation before you perform it.
A PSE detects PD disconnection in ac mode or dc mode. The ac mode uses less power than the dc mode.
2.     Configure a PD disconnection detection mode.
poe disconnect { ac | dc }
The default PD disconnection detection mode is ac.
About the maximum PI power
The maximum PI power is the maximum power that a PI can provide to the connected PD. If the PD requires more power than the maximum PI power, the PI does not supply power to the PD.
2.     Enter PI view.
3.     Configure the maximum power for the PI.
Versions
Default setting
The maximum PI power is 30000 W.
The maximum PI power is 35000 W.
PoE guard band is a specified amount of power reserved to prevent PSE power overload in case of PD power jitter. For example, if the maximum power of the PSE is 200 W and the guard band is 30 W, the PSE can provide a maximum power of 170 W to all PDs. If the total power of PDs reaches 170 W, no power will be supplied to new PDs.
When the PD operates stably with low power jitter (less than the default guard band), you can use the poe pse guard-band command to decrease the guard band and use the released PSE power to power the new PDs.
2.     Set the PoE guard band.
poe pse pse-id guard-band power
undo poe pse pse-id guard-band power
By default, the PoE guard band is 30 W.
About the PI priority policy
The PI priority policy enables the PSE to perform priority-based power allocation to PIs when PSE power overload occurs. The priority levels for PIs are critical, high, and low in descending order.
When PSE power overload occurs, the PSE supplies power to PDs as follows:
·     If the PI priority policy is disabled, the PSE supplies power to PDs depending on whether you have configured the maximum PSE power.
¡     If you have configured the maximum PSE power, the PSE does not supply power to the newly-added or existing PD that causes PSE power overload.
¡     If you have not configured the maximum PSE power, the PoE self-protection mechanism is triggered. The PSE stops supplying power to all PDs.
·     If the PI priority policy is enabled, the PSE supplies power to PDs as follows:
¡     If a PD being powered causes PSE power overload, the PSE stops supplying power to the PD.
¡     If a newly-added PD causes PSE power overload, the PSE supplies power to PDs in priority descending order of the PIs to which they are connected. If the newly-added PD and a PD being powered have the same priority, the PD being powered takes precedence. If multiple PIs being powered have the same priority, the PIs with smaller IDs takes precedence.
Before you configure a PI with critical priority, make sure the remaining power from the maximum PSE power minus the maximum powers of the existing PIs with critical priority is greater than maximum power of the PI.
Configuration for a PI whose power is preempted remains unchanged.
2.     Enable the PI priority policy.
poe pd-policy priority
By default, the PI priority policy is disabled.
3.     Enter PI view.
4.     (Optional.) Configure a priority for the PI.
By default, the priority for a PI is low.
About PSE power monitoring
The system monitors PSE power utilization and sends notification messages when PSE power utilization exceeds or drops below the threshold. If PSE power utilization crosses the threshold multiple times in succession, the system sends notification messages only for the first crossing. For more information about the notification message, see "Configuring SNMP."
2.     Configure a power alarm threshold for a PSE.
poe utilization-threshold value pse pse-id
By default, the power alarm threshold for a PSE is 80%.
Associating PoE with Track
The PoE module can collaborate with the Track module to monitor the link status between the device and a PD. For example, if the PD supports the NQA ICMP echo test, you can specify a track entry associated with NQA to test the reachability of the PD. The NQA ICMP echo test must be configured on a Layer 3 interface. The PI is a Layer 2 interface. You are required to create a VLAN interface for the ICMP echo test and assign the PI to the VLAN.
The Track module notifies the PoE module of the following monitoring results:
·     Positive—The monitored object is reachable.
·     Negative—The monitored object is unreachable.
·     NotReady—The monitoring result is not ready because of reasons such as nonexistence of the NQA group associated with the track entry.
When the Track module detects failure of the link, it changes the track entry state from positive to negative, which triggers the PoE module to take the following actions:
·     alarm-only: Outputs an SNMP notification and log.
·     alarm-reboot-pd: Outputs an SNMP notification and log and reboots the PD connected to the PI.
For information about SNMP notifications, see SNMP configuration in Network Management and Monitoring Configuration Guide.
For information about logs, see information center configuration in Network Management and Monitoring Configuration Guide.
For information about the Track module, see track configuration in High Availability Configuration Guide.
This feature is supported only in Release 6346 and later.
2.     Enter PI view.
3.     Associate the PI with a track entry.
poe track track-entry-number action { alarm | alarm-reboot-pd }
By default, a PI is not associated with a track entry.
To modify a PoE profile applied on a PI, first remove the PoE profile from the PI.
You can configure a PI either on the PI or by using a PoE profile. The poe max-power max-power and poe priority { critical | high | low } commands must be configured using the same method.
Configuring a PoE profile
2.     Create a PoE profile and enter its view.
poe-profile profile-name [ index ]
By default, no PoE profiles exist.
3.     Enable PoE.
poe enable
By default, PoE is disabled.
4.     (Optional.) Configure the maximum PI power.
Versions
Default setting
5.     (Optional.) Configure a PI priority.
The default priority is low.
This command takes effect only after the PI priority policy is enabled.
Applying a PoE profile
You can apply a PoE profile to multiple PIs in system view or a single PI in PI view. If you perform the operation in both views for the same PI, the most recent operation takes effect.
You can apply only one PoE profile to a PI.
Applying a PoE profile in system view
2.     Apply a PoE profile to PIs.
apply poe-profile { index index | name profile-name } interface interface-range
By default, a PoE profile is not applied to a PI.
Applying a PoE profile in PI view
2.     Enter PI view.
3.     Apply the PoE profile to the interface.
About upgrading PSE firmware in service
You can upgrade the PSE firmware in service in the following modes:
·     Refresh mode—Updates the PSE firmware without deleting it. You can use the refresh mode in most cases.
·     Full mode—Deletes the current PSE firmware and reloads a new one. Use the full mode if the PSE firmware is damaged and you cannot execute any PoE commands.
If the PSE firmware upgrade fails because of interruption such as a device reboot, you can restart the device and upgrade it in full mode again. After the upgrade, restart the device manually for the new PSE firmware to take effect.
2.     Upgrade the PSE firmware in service.
poe update { full | refresh } filename [ pse pse-id ]
Before supplying power to a PD, the device performs a detection of the PD. It supplies power to the PD only after the PD passes the detection. If the PD fails the detection but the power provided by the device meets the PD specifications, you can configure this task to enable forced power supply to the PD.
CAUTION
CAUTION:
This task enables the device to supply power to a PD directly without performing a detection of the PD. To avoid damaging the PD, make sure the power provided by the device meets the PD specifications before configuring this command.
This task is supported only in Release 6340 and later.
2.     Enter PI view.
3.     Enable forced PoE power supply.
poe force-power
By default, forced PoE power supply is disabled.
The Maintain Power Signature (MPS) is an electrical signature provided by a PD. The PD uses this signature to maintain connection to the PSE in sleep mode. The PD sends a PoE protocol-compliant pulse current to the PSE periodically. If the PSE detects the PoE protocol-compliant pulse current from the PD within the TMPDO, it supplies power to the PD. If the PSE does not detect the PoE protocol-compliant pulse current from the PD within the TMPDO, it will not supply power to the PD.
To send pulse currents at larger intervals for lower standby power, you can use this task to change the TMPDO to be longer.
This feature is supported only in R6349 and later.
Only PSE modules that have a model name of LSPPSE**A support this feature. To view the PSE models, execute the display poe pse command.
If you execute the command multiple times, the most recent configuration takes effect.
2.     Set the TMPDO for the MPS.
poe mps pse pse-id tmpdo { timer | long |normal }
By default, the normal TMPDO mode is used for the MPS. The TMPDO for the MPS is 324 milliseconds.
Display and maintenance commands for PoE
Display general PSE information.
display poe device [ slot slot-number ]
Display the power supplying information for the specified PI.
display poe interface [ interface-type interface-number ]
Display power information for PIs.
display poe interface power [ interface-type interface-number ]
Display detailed PSE information.
display poe pse [ pse-id ]
Display the power supplying information for all PIs on a PSE.
display poe pse pse-id interface
Display power information for all PIs on a PSE.
display poe pse pse-id interface power
Display all information about the PoE profile.
display poe-profile [ index index | name profile-name ]
Display all information about the PoE profile applied to the specified PI.
display poe-profile interface interface-type interface-number
PoE configuration examples
Example: Configuring PoE
As shown in Figure 2, configure PoE as follows:
·     Enable the device to supply power to IP telephones and APs.
·     Enable the device to supply power to IP telephones first when overload occurs.
·     Supply AP B with a maximum power of 9000 milliwatts.
Figure 2 Network diagram
# Enable the PI priority policy.
<PSE> system-view
[PSE] poe pd-policy priority
# Enable PoE on GigabitEthernet 1/0/1, GigabitEthernet 1/0/2, and GigabitEthernet 1/0/3, and configure their power supply priority as critical.
[PSE] interface gigabitethernet 1/0/1
[PSE-GigabitEthernet1/0/1] poe enable
[PSE-GigabitEthernet1/0/1] poe priority critical
[PSE-GigabitEthernet1/0/1] quit
[PSE] interface gigabitethernet 1/0/2
[PSE-GigabitEthernet1/0/2] poe enable
[PSE-GigabitEthernet1/0/2] poe priority critical
[PSE-GigabitEthernet1/0/2] quit
[PSE] interface gigabitethernet 1/0/3
[PSE-GigabitEthernet1/0/3] poe enable
[PSE-GigabitEthernet1/0/3] poe priority critical
[PSE-GigabitEthernet1/0/3] quit
# Enable PoE on GigabitEthernet 1/0/4 and GigabitEthernet 1/0/5, and set the maximum power of GigabitEthernet 1/0/5 to 9000 milliwatts.
[PSE] interface gigabitethernet 1/0/4
[PSE-GigabitEthernet1/0/4] poe enable
[PSE-GigabitEthernet1/0/4] quit
[PSE] interface gigabitethernet 1/0/5
[PSE-GigabitEthernet1/0/5] poe enable
[PSE-GigabitEthernet1/0/5] poe max-power 9000
# Connect the IP telephones and APs to the PSE to verify that they can obtain power and operate correctly. (Details not shown.)
Troubleshooting PoE
Failure to set the priority of a PI to critical
Symptom
Power supply priority configuration for a PI failed.
Solution
To resolve the issue:
1.     Identify whether the remaining guaranteed power of the PSE is lower than the maximum power of the PI. If it is, increase the maximum PSE power or reduce the maximum power of the PI.
2.     Identify whether the priority has been configured through other methods. If the priority has been configured, remove the configuration.
3.     If the issue persists, contact H3C Support.
Failure to apply a PoE profile to a PI
Symptom
PoE profile application for a PI failed.
Solution
1.     Identify whether some settings in the PoE profile have been configured. If they have been configured, remove the configuration.
2.     Identify whether the settings in the PoE profile meet the requirements of the PI. If they do not, modify the settings in the PoE profile.
3.     Identify whether another PoE profile is already applied to the PI. If it is, remove the application.
4.     If the issue persists, contact H3C Support.
