16-Security Command Reference
HomeSupportSwitchesS12500R SeriesReference GuidesCommand ReferencesH3C S12500R Switch Router Series Command References(R52xx)-6W10216-Security Command Reference
15-MACsec commands
15-MACsec commands 197.72 KB
MACsec commands
MACsec is supported only on the interfaces of the following service modules:
·     LSXM1CGMS48KBR1.
·     LSXM1CGQ72KCR1.
·     LSXM1CDMS36KCR1.
confidentiality-offset
Use confidentiality-offset to set the MACsec confidentiality offset in an MKA policy.
Use undo confidentiality-offset to restore the default.
confidentiality-offset offset-value
The MACsec confidentiality offset is 0. The entire frame is encrypted.
MKA policy view
offset-value: Specifies the confidentiality offset in bytes. The value can be 0, 30 or 50.
The MACsec confidentiality offset specifies the number of bytes starting from the frame header. MACsec encrypts only the bytes after the offset in a frame.
When an MKA policy is applied to a port, the MACsec confidentiality offset in the policy overwrites the confidentiality offset previously configured on the port. However, MACsec uses the confidentiality offset propagated by the key server.
The configured MACsec confidentiality offset cannot take effect when the GCM-AES-XPN-128 or GCM-AES-XPN-256 cipher suite is used. If the GCM-AES-XPN-128 or GCM-AES-XPN-256 cipher suite is used, the confidentiality offset is always 0.
# Set the MACsec confidentiality offset to 30 bytes in MKA policy abcd.
[Sysname] mka policy abcd
[Sysname-mka-policy-abcd] confidentiality-offset 30
macsec confidentiality-offset
mka apply policy
display macsec
Use display macsec to display MACsec information on ports.
display macsec [ interface interface-type interface-number ] [ verbose ]
interface interface-type interface-number: Specifies a port by its type and number. If you do not specify a port, this command displays MACsec information on all ports.
verbose: Displays detailed MACsec information. If you do not specify this keyword, the command displays brief MACsec information.
# Display brief MACsec information on HundredGigE 1/0/1.
<Sysname> display macsec interface hundredgige 1/0/1
Interface HundredGigE1/0/1
  Protect frames                : Yes
  Active MKA policy             : PL01
  Replay protection             : Enabled
  Config reply window size      : 0 frames
  Active replay window size     : 0 frames
  Config confidentiality offset : 0 bytes
  Active confidentinlity offset : 0 bytes
  Validation mode               : Check
# Display detailed MACsec information on HundredGigE 1/0/1.
<Sysname> display macsec interface hundredgige 1/0/1 verbose
  Config replay window size     : 0 frames
  Active confidentiality offset : 0 bytes
  Included SCI                  : No
  SCI conflict                  : No
  Cipher suite                  : GCM-AES-128
  MKA life time                 : 6 seconds
  Transmit secure channel:
    SCI           : 000C29F6A4380004
      Elapsed time: 00h:02m:19s
      Current SA  : AN 0        PN 1
  Receive secure channels:
    SCI           : 000C29258D430124
      Elapsed time: 00h:02m:17s
      Current SA  : AN 0        LPN 1
      Previous SA : AN N/A      LPN N/A
Protect frames
Status of MACsec desire on the port:
·     Yes.
·     No.
If the port does not have an MKA principal actor, this field displays N/A.
Active MKA policy
MKA policy applied to the port.
This field displays N/A if the port is not enabled with MACsec desire.
This field is not available if the port is enabled with MACsec desire but is not applied an MKA policy.
Replay protection
Status of replay protection on the port:
·     Enabled.
·     Disabled.
If the port is not enabled with MACsec desire, this field displays N/A.
Configured replay protection window size in number of frames.
This field displays N/A in the following situations:
·     The port is not enabled with MACsec desire.
·     The port is not enabled with replay protection.
Effective replay protection window size in number of frames.
Configured confidentiality offset in bytes.
Effective confidentiality offset in bytes.
Validation mode
Validation mode:
·     Check.
·     Disabled.
·     Strict.
Included SCI
Whether the frame includes SCI tag:
·     Yes.
·     No.
SCI conflict
Whether the SCI in the received MKA packets is the same as the local SCI:
·     Yes—The SCI in the received MKA packets is the same as the local SCI.
·     No—No MKA packet is received, or the SCI in the received MKA packets is different from the local SCI.
Cipher suite
Cipher suite for MACsec encryption:
·     GCM-AES-128.
·     GCM-AES-256.
·     GCM-AES-XPN-128.
·     GCM-AES-XPN-256.
MKA life time
MKA session keepalive timer.
Information about the secure channel for outbound traffic.
This field is not available if the port is not enabled with MACsec desire.
Information about the secure channel for inbound traffic.
Elapsed time
Lifetime of the secure channel.
SCI
A hexadecimal string that contains the MAC address and port ID.
Current SA
Current SA used by the secure channel.
If no current SA is available, each of the AN, PN, and LPN fields for the current SA displays N/A.
Previous SA
Previous SA used by the secure channel.
If no previous SA is available, each of the AN and LPN fields for the previous SA displays N/A.
PN
Packet number for outbound traffic.
AN
SA number.
LPN
The minimum received packet number allowed by SAK.
mka apply policy
display mka policy
Use display mka policy to display MKA policy information.
display mka { default-policy | policy [ name policy-name ] }
default-policy: Specifies the system-defined MKA policy.
policy: Specifies an MKA policy or all MKA policies.
name policy-name: Specifies an MKA policy by policy name. The policy-name argument represents the MKA policy name, a case-sensitive string of 1 to 16 characters. If you do not specify an MKA policy, this command displays information about all MKA policies.
# Display information about all MKA policies.
<Sysname> display mka policy
PolicyName          ReplayProtection   WindowSize    ConfOffset    Validation
default-policy      Yes                0             0             Check
policy1             Yes                0             30            Check
policy2             Yes                0             30            Check
policy3             No                 0             0             Strict
policy4             Yes                200           50            Check
policy5             Yes                0             0             Check
PolicyName
Name of the MKA policy.
ReplayProtection
Whether the replay protection feature is enabled.
WindowSize
Replay protection window size in number of frames.
ConfOffset
Confidentiality offset in bytes.
Validation
Validation mode:
·     Check.
·     Disabled.
·     Strict.
mka policy
mka apply policy
display mka session
Use display mka session to display MKA session information.
display mka session [ interface interface-type interface-number | local-sci sci-id ] [ verbose ]
interface interface-type interface-number: Specifies a port by its type and number. If you do not specify a port, this command displays MKA session information on all ports.
local-sci sci-id: Specifies a local SCI, a case-insensitive hexadecimal string of 16 characters.
verbose: Displays detailed MKA session information. If you do not specify this keyword, the command displays brief MKA session information.
# Display brief MKA session information on HundredGigE 1/0/1.
<Sysname> display mka session interface hundredgige 1/0/1
Tx-SCI    : 000C29F6A4380004
Priority  : 0
Capability: 3
  CKN for participant: ABCD
    Key server            : Yes
    MI (MN)               : D7B00EDA353242704CC6B0DB (7)
    Live peers            : 1
    Potential peers       : 0
    Principal actor       : Yes
    MKA session status    : Secured
    Confidentiality offset: 30 bytes
# Display detailed MKA session information on HundredGigE 1/0/1.
<Sysname> display mka session interface hundredgige 1/0/1 verbose
Priority  : 0
Capability: 3
    Key server            : Yes
    Live peers            : 1
    Potential peers       : 1
    Tx-SSCI               : 2
    Current SAK status    : Rx & Tx
    Current SAK AN        : 0
    Current SAK KI (KN)   : 4273791304C1C26259C94C3400000001 (1)
    Previous SAK status   : N/A
    Previous SAK AN       : N/A
    Previous SAK KI (KN)  : N/A
    Live peer list:
    MI                        MN         Prio  Cap  Rx-SCI            Rx-SSCI
    EA58DC3F8715953DBC6593F0  840        100   3    00E0020000000106  1
    Potential peer list:
    DA58DC3Q4573543DBC6699F0  3          200   3    00E0021200000107  N/A
Tx-SCI
SCI for outbound traffic, in hexadecimal notation.
Tx- SSCI
SSCI for outbound traffic when an XPN cipher suite is used. If no XPN cipher suite is used, this field displays N/A.
Priority/Prio
Key server priority, in the range of 0 to 255.
Capability/Cap
MACsec capability:
·     0—The port is MACsec incapable.
·     1—The port supports integrity check only.
·     2—The port supports integrity check and packet encryption. The confidentiality offset must be 0.
·     3—The port supports integrity check and packet encryption. The confidentiality offset can be 0, 30, or 50.
CKN for participant
CAK name of the MKA instance.
Key server
Whether the local end is the key server.
MI
Member identifier in hexadecimal notation.
MN
Message number.
Live peers
Numbers of peers that have already been learned.
Potential peers
Numbers of peers that are being negotiated.
Principal actor
Whether the MKA instance is the principal actor.
MKA instance refers to the operation entity of the MKA protocol on a port. A port might have multiple MKA instances. The principal actor is the MKA instance in active state.
MKA session status
MKA session status:
·     Unknown.
·     Pending.
·     Unauthenticated—The port has not been authenticated.
·     Secured—The session will be secured.
If the MKA instance is not the principal actor, this field displays N/A.
Confidentiality offset issued by the key server.
·     The packet is transmitted in plain text.
·     The MKA instance is not the principal actor.
Current SAK status
Status of the current SAK:
·     Tx—The SAK is used to send packets.
·     Rx—The SAK is used to receive packets.
·     The SAK does not exist.
Current SAK AN
SA number of the current SAK in use.
Current SAK KI
Key identifier of the current SAK in use, a string of hexadecimal digits that contains the key server's 12-byte MI and KN.
KN
SAK number.
Previous SAK status
Status of the previous SAK:
Previous SAK AN
SA number of the previous SAK.
Previous SAK KI
Key identifier of the previous SAK, a string of hexadecimal digits that contains the key server's 12-byte MI and KN.
Live peer list
List of peers that have participated in the MKA session.
This field is not available if no live peer exists.
Potential peer list
List of peers that are being negotiated.
This field is not available if no potential peer exists.
Rx-SCI
SCI for inbound traffic, in hexadecimal notation.
Rx-SSCI
SSCI for inbound traffic when an XPN cipher suite is used. If no XPN cipher suite is used, this field displays N/A.
reset mka session
display mka statistics
Use display mka statistics to display MKA statistics on ports.
display mka statistics [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies a port by its type and number. If you do not specify a port, this command displays MKA statistics on all ports.
# Display MKA statistics on HundredGigE 1/0/1.
<Sysname> display mka statistics interface hundredgige 1/0/1
Interface HundredGigE1/0/1 statistics
MKPDUs with invalid CKN : 0
MKPDUs with invalid ICV : 0
MKPDUs with Rx error    : 0
CKN for participant     : ABCD
  Tx MKPDUs             : 2379
  Rx MKPDUs             : 2375
  MKPDUs with invalid MN: 0
  MKPDUs with Tx error  : 0
  SAKs distributed      : 0
  SAKs received         : 5
Number of received MKA packets with invalid CKNs.
Number of MKA packets that failed ICV check.
Number of received error MKA packets.
CKN for participant
Tx MKPDUs
Number of the MKA packets sent by the MKA instance.
Rx MKPDUs
Number of the MKA packets received by the MKA instance.
Number of MKA packets with illegal MNs received by the MKA instance.
Number of error MKA packets sent by the MKA instance.
SAKs distributed
Number of SAKs distributed by the MKA instance.
SAKs received
Number of SAKs received by the MKA instance.
reset mka statistics
macsec cipher-suite
Use macsec cipher-suite to specify the cipher suite for MACsec encryption.
Use undo macsec cipher-suite to restore the default.
macsec cipher-suite { gcm-aes-128 | gcm-aes-256 [ standard ] | gcm-aes-xpn-128 | gcm-aes-xpn-256 [ standard ] }
MACsec uses the GCM-AES-128 cipher suite for encryption.
Ethernet interface view
gcm-aes-128: Specifies the GCM-AES-128 cipher suite.
gcm-aes-256: Specifies the GCM-AES-256 cipher suite.
gcm-aes-xpn-128: Specifies the GCM-AES-XPN-128 cipher suite.
gcm-aes-xpn-256: Specifies the GCM-AES-XPN-256 cipher suite.
standard: Specifies the standard cipher suite.
This command is supported only in device-oriented mode. Make sure the connected ports are configured with the same cipher suite. If the ports are configured with different cipher suites, they cannot successfully establish MKA sessions.
H3C's implementations of GCM-AES-256 and GCM-AES-XPN-256 cipher suites is slightly different from the standard open source cipher suites. To successfully establish MKA sessions with a peer using the standard open source GCM-AES-256 or GCM-AES-XPN-256 cipher suite for MACsec encryption, specify the standard keyword in the macsec cipher-suite command.
# Specify the GCM-AES-256 cipher suite for MACsec encryption on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] macsec cipher-suite gcm-aes-256
mka psk
Use macsec confidentiality-offset to set the MACsec confidentiality offset on a port.
Use undo macsec confidentiality-offset to restore the default.
macsec confidentiality-offset offset-value
The MACsec confidentiality offset on the port is 0. The entire frame is encrypted.
If you execute this command on a port to which an MKA policy has been applied, the configuration overwrites the confidentiality offset in the MKA policy. The MKA policy application is removed from the port. However, other settings (settings for parameters except the confidentiality offset) of the MKA policy are effective on the port.
MACsec uses the MACsec confidentiality offset propagated by the key server.
# Set the MACsec confidentiality offset to 30 bytes on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] macsec confidentiality-offset 30
display macsec
display mka session
mka apply policy
macsec desire
Use macsec desire to enable MACsec desire. The port expects MACsec protection for outbound frames.
Use undo macsec desire to disable MACsec desire.
macsec desire
undo macsec desire
MACsec desire is disabled. A port does not expect MACsec protection for outbound frames.
This command allows a MACsec port to expect MACsec protection for outbound frames. The key server determines whether MACsec protects the outbound frames.
MACsec protects the outbound frames of the port when the following requirements are met:
·     The key server is MACsec capable.
·     Both the local participant and its peer are MACsec capable.
·     A minimum of one participant is enabled with the MACsec desire feature.
# Enable MACsec desire on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] macsec desire
macsec mka-session log enable
Use macsec mka-session log enable to enable MKA session logging.
Use undo macsec mka-session log enable to disable MKA session logging.
MKA session logging is disabled.
This command enables the device to generate logs for MKA session changes, such as peer aging and SAK updates. The logs are sent to the information center of the device. For the logs to be output correctly, you must also configure the information center on the device. For more information about information center configuration, see Network Management and Monitoring Configuration Guide.
As a best practice, disable MKA session logging to prevent excessive log output.
# Enable MKA session logging.
[Sysname] macsec mka-session log enable
info-center source (Network Management and Monitoring Command Reference)
macsec replay-protection enable
Use macsec replay-protection enable to enable MACsec replay protection on a port.
Use undo macsec replay-protection enable to disable MACsec replay protection on a port.
MACsec replay protection is enabled on the port.
This feature allows a MACsec port to accept a number of out-of-order or repeated inbound frames.
If you execute this command on a port to which an MKA policy has been applied, the configuration overwrites the MACsec replay protection configuration in the MKA policy. The MKA policy application is removed from the port. However, other settings (settings for parameters except MACsec replay protection) of the MKA policy are effective on the port.
# Enable MACsec replay protection on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] macsec replay-protection enable
display macsec
macsec replay-protection window-size
mka apply policy
Use macsec replay-protection window-size to set the MACsec replay protection window size on a port.
Use undo macsec replay-protection window-size to restore the default.
macsec replay-protection window-size size-value
The MACsec replay protection window size is 0 on a port. The device accepts only frames that arrive in the correct order. Out-of-order or duplicated frames will be dropped.
size-value: Specifies the replay protection window size, in number of frames. If the GCM-AES-128 or GCM-AES-256 cipher suite is used, the value range for the replay protection window size is 0 to 4294967295. If the GCM-AES-XPN-128 or GCM-AES-XPN-256 cipher suite is used, the value range for the replay protection window size is 0 to 1073741823.
To allow a MACsec port to accept a number of out-of-order frames, enable replay protection and specify a replay protection window size on the port.
Suppose the replay protection window size is a on a port. After the port receives a packet with packet number (PN) x, it can accept only packets whose PN is greater than or equal to x-a.
The replay protection window size takes effect only when the replay protection feature is enabled on the port.
Set a replay protection window size based on the forwarding path of frames. If the frames might be forwarded multiple times, set a large replay protection window size.
If you execute this command on a port to which an MKA policy has been applied, the configuration overwrites the replay protection window size in the MKA policy. The MKA policy application is removed from the port. However, other settings (settings for parameters except the replay protection window size) of the MKA policy are effective on the port.
# Set the MACsec replay protection window size to 100 on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] macsec replay-protection window-size 100
display macsec
mka apply policy
macsec validation mode
Use macsec validation mode to set a MACsec validation mode on a port.
Use undo macsec validation mode to restore the default.
macsec validation mode { check | strict }
The MACsec validation mode is check on a port.
check: Performs validation only and does not drop illegal frames.
strict: Performs validation and drops illegal frames.
To avoid data loss, use the default validation mode check on the MACsec devices in case of MKA negotiation failure. After you use the display macsec command to verify that MKA negotiation has succeeded, change the validation mode to strict.
If you execute this command on a port to which an MKA policy has been applied, the configuration overwrites the validation mode in the MKA policy. The MKA policy application is removed from the port. However, other settings (settings for parameters except the validation mode) of the MKA policy are effective on the port.
# Set the MACsec validation mode to strict on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] macsec validation mode strict
display macsec
mka apply policy
validation mode
mka apply policy
Use mka apply policy to apply an MKA policy to a port.
Use undo mka apply policy to remove the MKA policy from a port.
mka apply policy policy-name
No MKA policy is applied to the port.
policy-name: Specifies the name of an MKA policy, a case-sensitive string of 1 to 16 characters.
An MKA policy defines MACsec parameters, including confidentiality offset, validation mode, replay protection, and replay protection window size.
When you apply an MKA policy to a port, the MACsec parameter settings in the policy overwrite the MACsec parameters previously configured on the port. Any modifications to the MKA policy take effect immediately.
When you remove the MKA policy from a port, the MACsec parameter settings on the port restore to the default.
The MKA policy applied to a port is automatically removed from that port when you delete the policy. No MKA policy will run on that port until after you apply one to it.
When you apply a nonexistent MKA policy to a port, the port automatically uses the system-defined MKA policy default-policy. After you create the specified policy, the policy will be automatically applied to the port.
# Apply MKA policy abcd to HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] mka apply policy abcd
display mka policy
validation mode
mka enable
Use mka enable to enable MKA on a port.
Use undo mka enable to disable MKA on a port.
mka enable
undo mka enable
MKA is disabled on a port.
MKA establishes and manages MACsec secure channels on a port. It also negotiates encryption keys used by MACsec.
The enabling of MKA on a port triggers MKA negotiation. After MKA negotiation succeeds, an MKA session is successfully established.
You cannot establish MACsec sessions on a hybrid port. On a trunk port, make sure the port permits the PVID to pass through. If the PVID is not in the list of permitted VLANs, MACsec session establishment might fail because of packet loss. For more information about the port link types, see VLAN configuration in Layer 2—LAN Switching Configuration Guide.
As a best practice to enable MKA on an aggregate interface, first use the shutdown command to shut down the interface. After enabling MKA on the aggregate interface, use the undo shutdown command to bring up the interface.
The following information applies only to interfaces on the LSXM1CGQ72KCR1 and LSXM1CDMS36KCR1 service modules:
·     When you enable or disable MKA on an interface, that interface goes down and then comes up again.
·     Packet drop occurs on an MKA-enabled interface when it forwards a 64-byte VLAN-tagged ARP packet with the tag removed. For more information about VLAN tag manipulation, see VLAN configuration in Layer 2—LAN Switching Configuration Guide.
·     The MACsec and Ethernet link aggregation features are mutually exclusive. On these service modules, you cannot assign an MKA-enabled interface to a link aggregation group or enable MKA on an interface already in a link aggregation group. For more information about Ethernet link aggregation, see Ethernet link aggregation configuration in Layer 2—LAN Switching Configuration Guide.
When you use interfaces on an LSXM1CGMS48KBR1 service module as aggregation group member interfaces, enabling or disabling MKA on the first member interface causes IS-IS flapping on the aggregate interface.
Configure the device as an MKA key server when the following conditions are met:
·     The device connects to an LSXM1CGQ72KC, LSXM1CDMS36KCR1, or LSXM1CDQ18KCR service module or an S12500R fixed-port switch.
·     MKA is enabled on the interface of the device that connects to the service module or S12500R fixed-port switch.
# Enable MKA on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] mka enable
display mka session
mka policy
Use mka policy to create an MKA policy and enter its view, or enter the view of an existing MKA policy.
Use undo mka policy to delete an MKA policy.
mka policy policy-name
undo mka policy policy-name
A system-defined MKA policy exists. The policy name is default-policy.
MKA policy provides a centralized method for configuring MACsec confidentiality offset, validation mode, replay protection, and replay protection window size.
The system supports multiple MKA policies.
You cannot delete or modify the system-defined MKA policy default-policy.
# Create an MKA policy named abcd and enter its view.
display mka policy
mka apply policy
validation mode
mka priority
Use mka priority to set the MKA key server priority.
Use undo mka priority to restore the default.
mka priority priority-value
undo mka priority
The MKA key server priority is 0.
priority-value: Specifies the priority value, in the range of 0 to 255. The priority is inversely related to its value.
The port that has higher priority (lower priority value) becomes the key server if you use a preshared key as the CAK. If the port and its peers have the same priority, MACsec compares the SCI values on the ports. The port with the lowest SCI value becomes the key server.
A port with priority 255 cannot become the key server. For a successful key server selection, make sure a minimum of one participant's key server priority is not 255.
Ports on the following service modules can act as key servers but not as key clients:
·     LSXM1CGQ72KCR1.
·     LSXM1CDMS36KCR1.
# Set the MKA key server priority to 2 on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] mka priority 2
display mka session
mka psk
Use mka psk to set a preshared key as the CAK.
Use undo mka psk to restore the default.
mka psk ckn name cak { cipher | simple } string
undo mka psk
No preshared key exists.
ckn name: Specifies the preshared key name, a hexadecimal string with an even number of case-insensitive characters. The name length is in the range of 2 to 64 characters.
cak: Specifies the preshared key.
cipher: Specifies the preshared key in encrypted form.
simple: Specifies the preshared key in plaintext form. For security purposes, the preshared key specified in plaintext form will be stored in encrypted form.
string: Specifies the preshared key. The plaintext form of the key is a hexadecimal string with an even number of case-insensitive characters, and the key length is in the range of 2 to 64 characters. The encrypted form of the key is a case-sensitive string of 2 to 117 characters.
The CAK can only be manually configured at the CLI.
You can execute this command to configure a preshared key on each MACsec port. Make sure the connected ports are configured with the same CKN and CAK. If the connected ports are configured with different CKNs and CAKs, they cannot successfully establish MKA sessions.
To successfully establish an MKA session between two connected ports, make sure only the ports are configured with the same CKN in the network.
To delete the configured keys for MKA sessions that have been established, perform the following tasks:
1.     Execute the undo mka psk command on the key server.
2.     Execute the undo mka psk command on the non-key server.
The deletion operation deletes the established MKA sessions at the same time.
Different cipher suites for MACsec encryption have different requirements for the CKN and CAK configuration.
·     The GCM-AES-128 cipher suite requires that the CKN and CAK each must be 32 characters long. If the configured CKN or CAK is not 32 characters long, the system performs the following operations when it runs the cipher suite:
¡     Automatically increases the length of the CKN or CAK by zero padding if the CKN or CAK contains less than 32 characters.
¡     Uses only the first 32 characters if the CKN or CAK contains more than 32 characters.
·     The GCM-AES-256 cipher suite requires that the CKN and CAK each must be 64 characters long. If the configured CKN or CAK contains less than 64 characters, the system automatically increases the length of the CKN or CAK by zero padding when it runs the cipher suite.
# Configure the CAK name as AB, and set the CAK to 1234 in plain text on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] mka psk ckn AB cak simple 1234
macsec cipher-suite
mka timer mka-life
Use mka timer mka-life to set the MKA life time.
Use undo mka timer mka-life to restore the default.
mka timer mka-life seconds
The MKA life time is 6 seconds.
seconds: Sets the MKA life time in seconds. The value range for this argument is 6 to 60.
The participants at each end of a secure session exchange MKA protocol packets to keep the session alive.
The MKA life time sets the session keepalive timer for participants. The timer starts on a participant when the participant receives the first MKA protocol packet from its peer. If the participant does not receive any subsequent MKA protocol packets from that peer before the timer expires, the participant determines that the session is insecure and then removes the session.
This command is applicable only in device-oriented mode.
Make sure the participants at each end of a secure session have the same MKA life time.
# Set the MKA life time to 10 seconds on HundredGigE 1/0/1.
[Sysname-HundredGigE1/0/1] mka timer mka-life 10
display macsec
Use replay-protection enable to enable MACsec replay protection in an MKA policy.
Use undo replay-protection enable to disable MACsec replay protection in an MKA policy.
MACsec replay protection is enabled in an MKA policy.
MKA policy view
When an MKA policy is applied to a port, the replay protection configuration in the policy overwrites the replay protection feature already used by the port.
# Enable MACsec replay protection in MKA policy abcd.
[Sysname-mka-policy-abcd] replay-protection enable
mka apply policy
Use replay-protection window-size to set the MACsec replay protection window size in an MKA policy.
Use undo replay-protection window-size to restore the default.
The MACsec replay protection window size in an MKA policy is 0. The device accepts only frames that arrive in the correct order. Out-of-order or duplicated frames will be dropped.
MKA policy view
The MACsec replay protection window size allows a MACsec port to accept a number of out-of-order inbound frames.
Suppose the replay protection window size is a on a port. After the port receives a packet with PN x, it can accept only packets whose PN is greater than or equal to x-a.
When an MKA policy is applied to a port, the replay protection window size in the policy overwrites the window size already configured on the port.
# Set the MACsec replay protection window size to 100 in MKA policy abcd.
[Sysname-mka-policy-abcd] replay-protection window-size 100
mka apply policy
reset mka session
Use reset mka session to reset MKA sessions on ports.
reset mka session [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies a port by its type and number. If you do not specify a port, this command resets MKA sessions on all ports.
This command first clears MKA sessions, and then immediately triggers a new session establishment negotiation.
# Reset MKA sessions on HundredGigE 1/0/1.
<Sysname> reset mka session interface hundredgige 1/0/1
display mka session
Use reset mka statistics to clear MKA statistics on ports.
reset mka statistics [ interface interface-type interface-number ]
interface interface-type interface-number: Specifies a port by its type and number. If you do not specify a port, this command clears MKA statistics on all ports.
# Clear MKA statistics on HundredGigE 1/0/1.
<Sysname> reset mka statistics interface hundredgige 1/0/1
validation mode
Use validation mode to set a MACsec validation mode in an MKA policy.
Use undo validation mode to restore the default.
The MACsec validation mode is check. The device performs validation only and does not drop illegal frames.
MKA policy view
When an MKA policy is applied to a port, the MACsec validation mode in the policy overwrites the MACsec validation mode already configured on the port.
# Set the MACsec validation mode to strict in MKA policy abcd.
[Sysname-mka-policy-abcd] validation mode strict
mka apply policy