01-EAA commands | 247.21 KB |
EAA commands
action cli
Use action cli to add a CLI action to a monitor policy.
Use undo action to remove an action.
undo action number
A monitor policy does not contain any actions.
CLI-defined policy view
number: Specifies an action ID in the range of 0 to 231.
cli command-line: Specifies the command line to be executed when the event occurs. You can enter abbreviated forms of command keywords, but you must make sure the forms can uniquely identify the command keywords. For example, you can enter int loop 1 for the interface loopback 1 command.
You can configure a series of actions to be executed in response to the event specified in a monitor policy. EAA executes the actions in ascending order of action IDs. When you add actions to a policy, you must make sure the execution order is correct. If two actions have the same ID, the most recent one takes effect.
To execute a command in a view other than user view, you must define actions required for accessing the target view before defining the command execution action. In addition, you must number the actions in the order they should be executed, starting with entering system view.
For example, to shut down an interface, you must create the following actions in order:
1. Action to enter system view.
2. Action to enter interface view.
3. Action to shut down the interface.
When you define an action, you can specify a value or specify a variable name for an argument. For more information about using EAA environment variables, see EAA configuration in Intelligent Operations Configuration Guide.
# Configure a CLI action for the CLI-defined policy test to shut down GigabitEthernet 1/0/1.
[Sysname] rtm cli-policy test
[Sysname-rtm-test] action 1 cli system-view
[Sysname-rtm-test] action 2 cli interface gigabitethernet 1/0/1
[Sysname-rtm-test] action 3 cli shutdown
action email
Use action email to add an email sending action to a monitor policy.
action number email receiver rx-list subject subject [ content content ]
undo action number
Predefined use roles
receiver rx-list: Specifies a space-separated list of email receivers.
subject subject: Specifies an email subject, a case-sensitive string of 1 to 255 characters that can contain environment variables.
content content: Specifies the email content, a case-sensitive string of 1 to 255 characters that can contain environment variables. If you do not specify this option, the email body is empty.
After you add this action to an EAA monitor policy, EAA generates and sends an email with the specified content to the designated receivers when the policy event occurs. You can use this feature to collect and send device O & M information to the administrators periodically.
# Add an email sending action to CLI-defined policy test, specifying [email protected] and [email protected] as the email receivers, [ALARM][SAMPLE] as the email subject, and test-msg as the email body.
[Sysname-rmt-test] action 4 email receiver [email protected],[email protected] subject [ALARM][SAMPLE] content test-msg
rtm email domain
rtm email max-size
rtm email username password
action reboot
Use action reboot to add a reboot action to a monitor policy.
action number reboot [ slot slot-number [ subslot subslot-number ] ]
undo action number
slot slot-number: Specifies an IRF member device by its member ID. If you do not specify a member device, the command reboots the IRF fabric.
subslot subslot-number: Specifies a subcard by its subslot number. If you do not specify a subcard, this command reboots the slot. Only the S5580X-HI series supports this option.
The reboot action configured with this command reboots devices or cards without saving the running configuration. If you want to save the running configuration, use the action cli command to configure reboot actions.
When you define an action, you can specify a value or specify a variable name for an argument. For more information about using EAA environment variables, see EAA configuration in Intelligent O&M Configuration Guide.
# Configure an action for the CLI-defined policy test to reboot the specified slot.
[Sysname-rtm-test] action 3 reboot slot 1
action switchover
Use action switchover to add an active/standby switchover action to a monitor policy.
action number switchover
undo action number
This command does not trigger a master/subordinate switchover in either of the following situations:
· No subordinate device is configured.
· The subordinate device is not in up state.
# Configure an action for the CLI-defined policy test to perform an active/standby switchover.
[Sysname-rtm-test] action 3 switchover
action syslog
Use action syslog to add a Syslog action to a monitor policy.
undo action number
priority priority: Specifies the log severity level in the range of 0 to 7. A lower value represents a higher severity level.
facility local-number: Specifies a logging facility by its facility number in the range of local0 to local7. Facility numbers are used by a log host to identify log creation facilities for filtering log messages.
msg msg-body: Configures the log message body.
EAA sends log messages to the information center. You can configure the information center to output these messages to certain destinations. For more information about the information center, see System Management Configuration Guide.
# Configure an action for the CLI-defined policy test to send a log message "hello" with a severity of 7 from the facility device local3.
[Sysname-rtm-test] action 3 syslog priority 7 facility local3 msg hello
commit
Use commit to enable a CLI-defined monitor policy.
commit
You must execute this command for a CLI-defined monitor policy to take effect.
After changing the settings in a policy that has been enabled, you must re-execute this command for the changes to take effect.
# Enable CLI-defined monitor policy test.
[Sysname-rtm-test] commit
display rtm environment
Use display rtm environment to display user-defined EAA environment variables and their values.
var-name: Specifies a user-defined EAA environment variable by its name, a case-sensitive string of 1 to 63 characters. The name can contain digits, letters, and the underscore sign (_), but its leading character cannot be the underscore sign. If you do not specify a variable, this command displays all user-defined EAA environment variables.
# Display all user-defined EAA environment variables.
<Sysname> display rtm environment
Name Value
save_cmd save main force
show_run_cmd display current-configuration
Name |
Name of a user-defined EAA environment variable. This field displays a maximum of 30 characters. To display a user-defined EAA environment variable name of more than 30 characters, use the display current-configuration command. |
Value |
Value of the user-defined EAA environment variable. This field displays a maximum of 30 characters. To display a user-defined EAA environment variable value of more than 30 characters, use the display current-configuration command. |
display rtm policy
Use display rtm policy to display information about EAA monitor policies.
active: Specifies policies that are executing the actions.
verbose: Displays detailed information about monitor policies.
policy-name: Specifies a policy by its name, a case-sensitive string of 1 to 63 characters. If you do not specify a policy, the command displays information about all monitor policies.
To display the running configuration of CLI-defined monitor policies, execute the display current-configuration command in any view or execute the display this command in CLI-defined monitor policy view.
# Display monitor policies that are executing the actions.
<Sysname> display rtm policy active
JID Type Event TimeActive PolicyName
507 CLI INTERFACE Aug 29 14:55:55 2019 test
JID |
Job ID, displayed only when you specify the active keyword. |
Type |
Policy creation method: · TCL—The policy was configured by using Tcl. · CLI—The policy was configured from the CLI. |
Event |
Event type, including CLI, interface, process, SNMP, SNMP-Notification, syslog, and track. |
TimeActive |
Time when the monitor policy was triggered. |
PolicyName |
Name of the monitor policy. |
# Display brief information about all created monitor policies.
Total number: 1
Type Event TimeRegistered PolicyName
CLI INTERFACE Aug 29 14:54:50 2019 test
Total number |
Total number of the monitor policies. |
Type |
Event |
Event type, including CLI, hotplug, interface, process, SNMP, SNMP-Notification, Syslog, and track. |
TimeRegistered |
Time when the monitor policy was created. |
PolicyName |
# Display detailed information about all monitor policies.
<Sysname> display rtm policy registered verbose
Total number: 1
Policy Name: test
Policy Type: CLI
Event Type: INTERFACE
TimeRegistered: Aug 29 14:54:50 2019
User-role: network-operator
Total number |
Total number of the monitor polices. |
PolicyName |
Policy Type |
Event Type |
TimeRegistered |
Time when the policy was created. |
User-role |
User roles for executing the monitor policy. To execute the monitor policy, an administrator must have a minimum of one of the displayed user roles. |
display rtm policy history
Use display rtm policy history to display history execution records for EAA monitor policies.
display rtm policy history [ policy-name ]
policy-name: Specifies a policy by its name, a case-sensitive string of 1 to 63 characters. If you do not specify a policy, the command displays history execution records for all monitor policies.
The device can display a maximum of 32 history execution records for an EAA monitor policy.
# Display history execution records for monitor policies.
<Sysname> display rtm policy history
Task ID: 2
Policy name: cfgchage
Event occurred at: Mar 27 08:45:35 2023
Event recovered at: -NA-
Environment variables:
Name Value
_event_id 3
_event_severity 0
_event_taskid 2
_event_time Mon Mar 27 08:45:35 2023
_event_type SYSLOG
_event_type_string SYSLOG_EVENT
_syslog_pattern <1477>Mar 27 08:45:35 2023 Sysname %%10CFGMAN
/5/CFGMAN_CFGCHANGED: -EventIndex=2-CommandSource=snmp-ConfigSource=startup-Conf
igDestination=running; Configuration changed.
Script information:
Script name : /sbin/python/eaa/policy/cfgchage.py
Started at : Mar 27 08:45:35 2023
Ended at : Mar 27 08:45:35 2023
Result : Successful
Policy execution result: Success
Task ID: 1
Event occurred at: Mar 27 07:55:35 2023
Name Value
_event_id 3
_event_severity 0
_event_taskid 1
_event_time Mon Mar 27 07:55:35 2023
_event_type SYSLOG
_syslog_pattern <1477>Mar 27 07:55:35 2023 Sysname %%10CFGMAN
/5/CFGMAN_CFGCHANGED: -EventIndex=1-CommandSource=snmp-ConfigSource=startup-Conf
Script information:
Started at : Mar 27 07:55:35 2023
Ended at : Mar 27 07:55:35 2023
Result : Successful
Table 5 Command output
Task ID |
ID of the task for running an EAA monitor policy. |
Event recovered at |
Time when the event recovered. If this field displays NA, the event bound to the policy has not recovered. |
Script information: Script name: Started at : Ended at : Result : Failure reason: |
Information about the test script associated with the EAA monitor policy: · Script name. · Time when the script was run. · Time when the script stopped running. · Script execution result: ¡ Success. ¡ Failed. · Reason when the script failed to be executed: |
EAA module test information: Test name: Started at : Ended at : Result : Failure reason: |
Information about the EAA test associated with the EAA monitor policy. If no EAA test is associated, this field is not displayed. · EAA test name. · Time when the EAA test started to be executed. · Time when the EAA test stopped to be executed. · Execution result of the EAA test: ¡ Success. ¡ Failed. · Reason why the EAA test failed be executed: |
Policy execution result |
Execution result of the EAA monitor policy: · Success. · Failed. |
event cli
Use event cli to configure a CLI event for a CLI-defined monitor policy.
Use undo event to delete the event in a CLI-defined monitor policy.
undo event
No CLI event is configured.
async [ skip ]: Enables or disables the system to execute the command that triggers the policy. If you specify the skip keyword, the system executes the actions in the policy without executing the command that triggers the policy. If you do not specify the skip keyword, the system executes both the actions in the policy and the command entered at the CLI.
sync: Enables the system to execute the command that triggers the event only if the policy has been executed successfully.
mode { execute | help | tab }: Specifies the CLI operation to monitor:
· execute: Triggers the policy when a matching command is entered.
· help: Triggers the policy when a question mark (?) is entered at a matching command line.
· tab: Triggers the policy when the Tab key is pressed to complete a parameter in a matching command line.
pattern regular-exp: Specifies a regular expression for matching commands that trigger the policy. For more information about using regular expressions, see CLI in Fundamentals Configuration Guide.
Use CLI event monitor policies to monitor operations performed at the CLI.
You can configure only one event for a monitor policy. If the monitor policy already contains an event, the new event replaces the old event.
# Configure a CLI-defined policy to monitor execution of commands that contain the display interface brief string. Enable the system to execute the actions in the policy without executing the command that triggers the policy.
<Sysname>system-view
[Sysname-rmt-test] event cli async skip mode execute pattern display interface brief
# Configure a CLI-defined policy to monitor the use of the Tab key at command lines that contain the display interface brief string. Enable the system to execute the actions in the policy and display the complete parameter when Tab is pressed at a policy-matching command line.
[Sysname-rmt-test] event cli async mode tab pattern display interface brief
# Configure a CLI-defined policy to monitor the use of the question mark (?) at command lines that contain the display interface brief string. Enable the system to execute a policy-matching command line only if the actions in the policy are executed successfully when a question mark is entered at the command line.
[Sysname-rmt-test] event cli sync mode help pattern display interface brief
event hotplug
Use event hotplug to configure a hot-swapping event.
event hotplug [ insert | remove ] slot slot-number [ subslot subslot-number ]
undo event
No hotplug event is configured.
insert: Specifies the IRF member device join event and subcard insert event.
remove: Specifies the IRF member device leave event and subcard remove event.
subslot subslot-number: Specifies a subcard by its subslot number. If you do not specify a subcard, EAA monitors the slot for hot-swapping events. Only the S5580X-HI supports this parameter.
After you configure the event, the monitor policy is triggered when the member device joins or leaves the IRF fabric, or when a subcard is inserted in or removed from the specified subcard slot. If you do not specify the insert or remove keyword, EAA monitors the member device for joining or leaving the IRF fabric and the subcard slot for subcard hot-swapping.
You can configure only one event entry for a monitor policy. If the monitor policy already contains an event entry, the new event entry replaces the old event entry.
# Configure a CLI-defined policy to monitor the member device for joining or leaving the IRF fabric.
[Sysname-rtm-test] event hotplug slot 1
event interface
Use event interface to configure an interface event for a CLI-defined monitor policy.
event interface monitor-interface-list monitor-obj monitor-obj start-op start-op start-val start-val restart-op restart-op restart-val restart-val [ interval interval ]
event interface all monitor-obj monitor-obj start-op start-op start-val start-val restart-op restart-op restart-val restart-val [ interval interval ] exclude exclude-interface-list
undo event
No interface event is configured.
monitor-interface-list: Specifies a space-separated list of up to 8 interface items to monitor. Each item specifies an interface or a range of interfaces in the form of interface-type interface-number1 [ to interface-type interface-number2 ]. The value for interface-number2 must be greater than or equal to the value for interface-number1. The specified interfaces must be the same type and on the same interface module or subcard.
all: Specifies all interfaces.
monitor-obj monitor-obj: Specifies the traffic statistic to be monitored on the interface. For keywords available for the monitor-obj argument, see Table 6.
start-op start-op: Specifies the operator for comparing the monitored traffic statistic with the start threshold. The start threshold is crossed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 7.
start-val start-val: Specifies the start threshold to be compared with the monitored traffic statistic. The value range is 0 to 4294967295.
restart-op restart-op: Specifies the operator for comparing the monitored traffic statistic with the restart threshold. The restart threshold is crossed if the comparison result meets the condition. For keywords available for the restart-op argument, see Table 7.
restart-val restart-val: Specifies the restart threshold to be compared with the monitored traffic statistic. The value range is 0 to 4294967295.
interval interval: Specifies the interval to sample the monitored traffic statistic for a comparison. The value range is 1 to 4294967295, in seconds. The default value is 300.
exclude exclude-interface-list: Specifies a space-separated list of up to 8 interface items to be excluded from monitoring. Each item specifies an interface or a range of interfaces in the form of interface-type interface-number1 [ to interface-type interface-number2 ]. The value for interface-number2 must be greater than or equal to the value for interface-number1. The specified interfaces must be the same type and on the same interface module or subcard.
Monitored traffic statistic |
input-drops |
Number of discarded incoming packets during the sampling interval |
input-errors |
Number of incoming error packets during the sampling interval |
output-drops |
Number of discarded outgoing packets during the sampling interval |
output-errors |
Number of outgoing error packets during the sampling interval |
rcv-bps |
Receive rate, in bps during the sampling interval |
rcv-broadcasts |
Number of incoming broadcasts during the sampling interval |
rcv-pps |
Receive rate, in packets per second |
tx-bps |
Transmit rate, in bps |
tx-pps |
Transmit rate, in packets per second |
Comparison operator |
eq |
Equal to |
ge |
Greater than or equal to |
gt |
Greater than |
le |
Less than or equal to |
lt |
Less than |
ne |
Not equal to |
Use interface event monitor policies to monitor traffic statistics on an interface.
EAA executes an interface event policy when the monitored interface traffic statistic crosses the start threshold in the following situations:
· The statistic crosses the start threshold for the first time.
· The statistic crosses the start threshold each time after it crosses the restart threshold.
The following is the interface event monitor process of EAA:
1. Compares the traffic statistic sample with the start threshold at sampling intervals until the start threshold is crossed.
2. Executes the policy.
3. Compares the traffic statistic sample with the restart threshold at sampling intervals until the restart threshold is crossed.
4. Compares the traffic statistic sample with the start threshold at sampling intervals until the start threshold is crossed.
5. Executes the policy again.
This process cycles for the monitor policy to be executed and re-executed.
# Configure a CLI-defined policy to monitor the incoming error packet statistic on GigabitEthernet 1/0/1 every 60 seconds. Set the start threshold to 1000 and the restart threshold to 50. Enable EAA to execute the policy when the statistic exceeds 1000 for the first time. Enable EAA to re-execute the policy if the statistic exceeds 1000 each time after the statistic has dropped below 50.
[Sysname-rtm-test] event interface gigabitethernet 1/0/1 monitor-obj input-errors start-op gt start-val 1000 restart-op lt restart-val 50 interval 60
# Configure a CLI-defined policy to monitor the incoming error packet statistic on interfaces except GigabitEthernet 1/0/1 every 60 seconds. Set the start threshold to 1000 and the restart threshold to 50. Enable EAA to execute the policy when the statistic exceeds 1000 for the first time. Enable EAA to re-execute the policy if the statistic exceeds 1000 each time after the statistic has dropped below 50.
[Sysname-rtm-test] event interface all monitor-obj input-errors start-op gt start-val 1000 restart-op lt restart-val 50 interval 60 exclude gigabitethernet 1/0/1
event period
Use event period to configure a periodic event for a CLI-defined monitor policy.
event period interval
undo event
No periodic event is configured for a monitor policy.
interval: Specifies the periodic event interval in the range of 1 to 43200, in minutes.
Operating mechanism
After you configure this event for an EAA monitory policy, EAA executes the policy when the interval expires and then starts the timer for the next interval.
You can configure only one event entry for a monitor policy. If you configure multiple event entries for a monitor policy, the most recent configuration takes effect.
For the actions of a periodic event monitor policy to be executed completely, the interval configured for the periodic event must be equal to or larger than the action running time.
# Set the periodic event interval to 60 minutes.
[Sysname-rtm-test] event period 60
running-time
event process
Use event process to configure a process event for a CLI-defined monitor policy.
undo event
No process event is configured.
exception: Monitors the specified process for exceptional events. EAA executes the policy when an exception occurs to the monitored process.
restart: Monitors the specified process for restart events. EAA executes the policy when the monitored process restarts.
shutdown: Monitors the specified process for shutdown events. EAA executes the policy when the monitored process is shut down.
start: Monitors the specified process for start events. EAA executes the policy when the monitored process starts.
name process-name: Specifies a user-mode process by its name. The process can be one that is running or not running. If you do not specify a name, this command monitors all use-mode processes.
instance instance-id: Specifies a process instance ID in the range of 0 to 4294967294. The instance ID can be one that has not been created yet. If you do not specify an instance, EAA monitors all instances of the process.
slot slot-number: Specifies an IRF member device by its member ID. If you do not specify a member device, this command applies to the IRF fabric.
Use process event monitor policies to monitor process state changes. These changes can result from manual operations or automatic system operations.
# Configure a CLI-defined policy to monitor all instances of the process snmpd for restart events.
[Sysname-rtm-test] event process restart name snmpd
event snmp oid
Use event snmp oid to configure an SNMP event for a CLI-defined monitor policy.
undo event
No SNMP event is configured.
oid oid: Specifies the OID of the monitored MIB variable, a string of 1 to 256 characters.
monitor-obj { get | next }: Specifies the SNMP operation used for sampling variable values. The get keyword represents the SNMP get operation, and the next keyword represents the SNMP getNext operation.
start-op start-op: Specifies the operator for comparing the sampled value with the start threshold. The start threshold is crossed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 7.
start-val start-val: Specifies the start threshold to be compared with the sampled value. The start-val argument can be any data type supported by SNMP, including numerals and character strings. The value range for the start-val argument is a string of 1 to 512 characters. If the threshold value contains spaces, you must enclose the value in quotation marks (" ").
restart-op op: Specifies the operator for comparing the sampled value with the restart threshold. The restart threshold is crossed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 7.
restart-op restart-val: Specifies the restart threshold to be compared with the sampled value. The restart-val argument can be any data type supported by SNMP, including numerals and character strings. The value range for the restart-val argument is a string of 1 to 512 characters. If the threshold value contains spaces, you must enclose the value in quotation marks (" ").
interval interval: Specifies the sampling interval in the range of 1 to 4294967295, in seconds. The default value is 300.
Use SNMP event monitor policy to monitor value changes of MIB variables.
EAA executes an SNMP event policy when the monitored MIB variable's value crosses the start threshold in the following situations:
· The monitored variable's value crosses the start threshold for the first time.
· The monitored variable's value crosses the start threshold each time after it crosses the restart threshold.
The following is the SNMP event monitor process of EAA:
1. Compares the variable sample with the start threshold at sampling intervals until the start threshold is crossed.
3. Compares the variable sample with the restart threshold at sampling intervals until the restart threshold is crossed.
4. Compares the variable sample with the start threshold at sampling intervals until the start threshold is crossed.
For the command to take effect, enable SNMP before you execute this command.
# Configure a CLI-defined policy to get the value of the MIB variable 1.3.6.4.9.9.42.1.2.1.6.4 every five seconds. Set the start threshold to 1 and the restart threshold to 2. Enable EAA to execute the policy when the value changes to 1 for the first time. Enable EAA to re-execute the policy if the value changes to 1 each time after the value has changed to 2.
[Sysname-rtm-test] event snmp oid 1.3.6.4.9.9.42.1.2.1.6.4 monitor-obj get start-op eq start-val 1 restart-op eq restart-val 2 interval 5
event snmp-notification
Use event snmp-notification to configure an SNMP-Notification event for a CLI-defined policy.
Use undo event to remove the event in a CLI-defined policy.
undo event
No SNMP-Notification event is configured.
oid-val oid-val: Specifies the threshold to be compared with the sampled value. The oid-val argument can be any data type supported by SNMP, including numerals and character strings. The value range for the oid-val argument is a string of 1 to 512 characters. If the threshold value contains spaces, you must enclose the value in quotation marks (" ").
op op: Specifies the operator for comparing the sampled value with the threshold. The policy is executed if the comparison result meets the condition. For keywords available for the start-op argument, see Table 7.
drop: Drops the notification if the comparison result meets the condition. If you do not specify this keyword, the system sends the notification.
Use SNMP-Notification event monitor policies to monitor variables in SNMP notifications.
EAA executes an SNMP-Notification event monitor policy when the value of the monitored variable in an SNMP notification meets the specified condition.
# Configure a CLI-defined policy to monitor SNMP notifications that contain the use name variable 1.3.6.1.4.1.25506.2.2.1.1.2.1.0. Enable the system to execute the policy and drop the SNMP notification if the use name variable value is admin.
[Sysname-rtm-test] event snmp-notification oid 1.3.6.1.4.1.25506.2.2.1.1.2.1.0 oid-val admin op eq drop
event syslog
Use event syslog to configure a Syslog event for a CLI-defined monitor policy.
event syslog priority { priority | all } msg msg occurs times period period
undo event
No Syslog event is configured.
priority { priority | all }: Specifies the severity level for matching log messages.
· priority: Specifies the lowest severity level for matching log messages. It is an integer in the range of 0 to 7. A lower number represents higher severity level. For example, specify a severity level of 3 to match log messages from level 3 to level 0.
· all: Represents any severity level from 0 to 7.
msg msg: Specifies a regular expression to match the logs. The msg argument represents a regular expression, a string of 1 to 255 characters.
occurs times period period: Executes the policy if the number of log matches over an interval exceeds the limit. The times argument specifies the maximum number of log matches in the range of 1 to 32. The period argument specifies an interval in the range of 1 to 4294967295 seconds.
Use Syslog event monitor policies to monitor log messages.
EAA executes a Syslog event monitor policy when the number of matching logs over an interval reaches the limit.
NOTE: EAA does not count log messages generated by the RTM module when it counts log matches. |
A regular expression can contain the special characters described in Table 8.
Table 8 Special characters supported in a regular expression
Characters |
Meaning |
Examples |
Matches the beginning of a line. |
"^u" matches all lines beginning with "u". A line beginning with "Au" is not matched. |
Matches the end of a line. |
"u$" matches all lines ending with "u". A line ending with "uA" is not matched. |
. (period) |
Matches any single character. |
".s" matches "as" and "bs". |
Matches the preceding character or string zero, one, or multiple times. |
"zo*" matches "z" and "zoo", and "(zo)*" matches "zo" and "zozo". |
Matches the preceding character or string one or multiple times. |
"zo+" matches "zo" and "zoo", but not "z". |
Matches the preceding or succeeding string. |
"def|int" matches a line containing "def" or "int". |
Matches the string in the parentheses, usually used together with the plus sign (+) or asterisk sign (*). |
"(123A)" matches "123A". "408(12)+" matches "40812" and "408121212", but not "408". |
\N |
Matches the preceding strings in parentheses, with the Nth string repeated once. |
"(string)\1" matches a string containing "stringstring". "(string1)(string2)\2" matches a string containing "string1string2string2". "(string1)(string2)\1\2" matches a string containing " string1string2string1string2". |
Matches a single character in the brackets. |
"[16A]" matches a string containing 1, 6, or A; "[1-36A]" matches a string containing 1, 2, 3, 6, or A (- is a hyphen). To match the character "]", put it immediately after "[", for example, []abc]. There is no such limit on "[". |
Matches a single character that is not in the brackets. |
"[^16A]" matches a string that contains one or more characters except for 1, 6, or A, such as "abc". A match can also contain 1, 6, or A (such as "m16"), but it cannot contain these three characters only (such as 1, 16, or 16A). |
{n} |
Matches the preceding character n times. The number n must be a nonnegative integer. |
"o{2}" matches "food", but not "Bob". |
{n,} |
Matches the preceding character n times or more. The number n must be a nonnegative integer. |
"o{2,}" matches "foooood", but not "Bob". |
{n,m} |
Matches the preceding character n to m times or more. The numbers n and m must be nonnegative integers and n cannot be greater than m. |
" o{1,3}" matches "fod", "food", and "foooood", but not "fd". |
Matches a string that starts with the pattern following \<. A string that contains the pattern is also a match if the characters preceding the pattern are not digits, letters, or underscores. |
"\<do" matches "domain" and "doa". |
Matches a string that ends with the pattern preceding \>. A string that contains the pattern is also a match if the characters following the pattern are not digits, letters, or underscores. |
"do\>" matches "undo" and "cdo". |
\b |
Matches a word that starts with the pattern following \b or ends with the pattern preceding \b. |
"er\b" matches "never", but not "verb" or "erase". "\ber" matches "erase", but not "verb" or "never". |
\B |
Matches a word that contains the pattern but does not start or end with the pattern. |
"er\B" matches "verb", but not "never" or "erase". |
\w |
Same as [A-Za-z0-9_], matches a digit, letter, or underscore. |
"v\w" matches "vlan" and "service". |
\W |
Same as [^A-Za-z0-9_], matches a character that is not a digit, letter, or underscore. |
"\Wa" matches "-a", but not "2a" or "ba". |
Escape character. If a special character listed in this table follows \, the specific meaning of the character is removed. |
"\\" matches a string containing "\", "\^" matches a string containing "^", and "\\b" matches a string containing "\b". |
# Configure a CLI-defined policy to monitor Syslog messages for level 3 to level 0 messages that contain the down string. Enable the policy to execute when five log matches are found within 6 seconds.
[Sysname-rtm-test] event syslog priority 3 msg down occurs 5 period 6
event track
Use event track to configure a track event for a CLI-defined monitor policy.
undo event
A CLI-defined policy does not contain a track event.
track-list: Specifies a space-separated list of up to 16 track items. Each item specifies a track entry number or a range of track entry numbers in the form of track-entry-number to track-entry-number. The value range for the track-entry-number argument is 1 to 1024.
state { negative | positive }: Monitors state change of the track entries.
· negative: Triggers the policy when the states of the track entries change from Positive to Negative.
· positive: Triggers the policy when the states of the track entries change from Negative to Positive.
suppress-time suppress-time: Sets a suppress time in the range of 1 to 4294967295, in seconds. The default value is 0.
After you configure a track event for an EAA monitor policy, the track event occurs and triggers the policy when the state of the track entry changes from Positive to Negative or from Negative to Positive. If you specify multiple track entries for a policy, the policy is triggered only when the state of all the track entries changes from Positive to Negative or Negative to Positive.
For example, for the sessions between the local device and its downlink BGP peers to disconnect automatically when the sessions between the local device and its uplink BGP peers are disconnected, you can configure a track event monitor policy as follows:
· Configure a track event for the policy and specify track entries to monitor the links between the local device and its uplink BGP peers.
· Add the CLI action peer ignore to the policy to disable BGP session establishment between the local device and its downlink BGP peers.
To avoid frequent triggering of the EAA monitor policy by the track event, you can specify suppression time to control the interval between executions of the monitor policy. After the suppression time is configured, the policy is triggered and the suppression timer is started when the track event occurs for the first time.
· If the track event occurs again before or when the suppression timer expires, the track event will be suppressed and will not trigger the monitor policy.
· If the track event occurs again after the suppression timer expires, the monitor policy is triggered and the suppression timer will be reset and restart timing until the monitor policy is stopped.
For example, if you execute the track 1 interface gigabiteethernet 1/0/1 and event track 1 state negative suppress-time 60 commands to configure a track event for a monitor policy, the following occurs:
· When the state of interface GigabitEthernet1/0/1 changes to down for the first time, the monitor policy is triggered.
· If the state of interface GigabitEthernet1/0/1 changes to down again within 60 seconds, the monitor policy will not be triggered. This prevents frequent triggering of the monitor policy within one minute in case of state flapping of GigabitEthernet1/0/1.
· If the state of interface GigabitEthernet1/0/1 changes to down again after 1 minute, the monitor policy is triggered.
# Create CLI-defined monitor policy test. Configure a track event for the policy that occurs when the states of track entry 1 to track entry 8 change from Positive to Negative. Set the suppress time to 180 seconds for the policy.
[Sysname-rtm-test] event track 1 to 8 state negative suppress-time 180
rtm cli-policy
Use rtm cli-policy to create a CLI-defined EAA monitor policy and enter its view, or enter the view of an existing CLI-defined EAA monitor policy.
Use undo rtm cli-policy to delete a CLI-defined monitor policy.
rtm cli-policy policy-name
undo rtm cli-policy policy-name
No CLI-defined monitor policies exist.
policy-name: Specifies the name of a CLI-defined monitor policy, a case-sensitive string of 1 to 63 characters.
You must create a CLI-defined monitor policy before you can use the CLI to configure settings in the policy.
For a CLI-defined monitor policy to take effect, you must execute the commit command after you complete configuring the policy.
You can execute this command multiple times to create multiple CLI-defined monitor policies. Make sure the CLI-defined monitor policies that are executed at the same time do not have conflicting actions. If the actions conflict, the system executes the actions randomly.
You can assign the same name to a CLI-defined policy and a Tcl-defined policy.
# Create a CLI-defined policy and enter its view.
commit
rtm email domain
Use rtm email domain to specify an email server domain name.
Use undo rtm email domain to restore the default.
rtm email domain domain-name
No email server domain name is specified.
domain-name: Specifies the email server domain name, a case-sensitive string of 1 to 255 characters. The name cannot contain a forward slash (/), backslash (\), vertical bar (|), quotation marks ("), colon (:), asterisk (*), question mark (?), left angle bracket (<), right angle bracket (>), or at sign (@).
After you specify an email server address by its domain name, you do not need to reconfigure the email server address when the email server address changes.
# Specify 163.com as the email server domain name.
[Sysname] rtm email domain 163.com
action email
rtm email max-size
rtm email max-size
Use rtm email max-size to set the maximum email size that the device can send.
Use undo rtm email max-size to restore the default.
rtm email max-size size
The device can send an email with a maximum size of 2 MB.
size: Specifies the maximum email size in the range of 1 to 50, in MB.
For an email to be sent correctly, make sure the email size does not exceed the value specified by this command and the maximum email size configured on the email server.
# Set the maximum email size that the device can send to 10 MB.
[Sysname] rtm email max-size 10
rtm email domain
Use rtm email username password to set the email username and password.
Use undo rtm email username to restore the default.
rtm email username username password { simple | cipher} password
No email username or password exists.
username: Specifies an email username, a case-insensitive string of 1 to 31 characters that do not contain the domain name.
cipher: Specifies an email password in encrypted form.
simple: Specifies an email password in plaintext form. The password will be saved in encrypted form.
password: Sets a case-sensitive password. The password is a string of 1 to 31 characters in plaintext form or a string of 33 to 73 characters in encrypted form.
For an email to be sent correctly, make sure the email username and password are consistent with those registered with the email server.
# Set both the email username and password to test.
[Sysname] rtm email username test password simple test
rtm email domain
rtm environment
Use rtm environment to configure an EAA environment variable.
Use undo rtm environment to delete a user-defined EAA environment variable.
undo rtm environment var-name
No user-defined EAA environment variables exist.
The system provides the variables in Table 9. You cannot create, delete, or modify these system-defined variables.
Table 9 System-defined EAA environment variables by event type
Event |
Variable name and description |
Any event |
_event_id: Event ID _event_type: Event type _event_type_string: Event type description _event_time: Time when the event occurs _event_severity: Severity level of an event |
CLI |
_cmd: Commands that are matched |
Hotplug |
_slot: ID of the member device that joins or leaves the IRF fabric |
Hotplug |
_subslot: ID of the subslot where subcard hot-swapping occursOnly the S5580X-HI switch series supports this field. |
_ifname: Interface name |
Period |
_period_value: Interval. |
Process |
_process_name: Process name. |
SNMP |
_oid: OID of the MIB variable where an SNMP operation is performed _oid_value: Value of the MIB variable |
SNMP-Notification |
_oid: OID that is included in the SNMP notification. |
Syslog |
_syslog_pattern: Log message content. |
var-value: Specifies the variable value.
When you define an action, you can enter a variable name with a leading dollar sign ($variable_name) instead of entering a value for an argument. EAA will replace the variable name with the variable value when it performs the action.
For an action argument, you can specify a list of variable names in the form of $variable_name1$variable_name2...$variable_nameN.
# Create an environment variable: set its name to if and set its value to interface.
[Sysname] rtm environment if interface
rtm event syslog buffer-size
Use rtm event syslog buffer-size to set the size for the EAA-monitored log buffer.
Use undo rtm event syslog buffer-size to restore the default.
The size of the EAA-monitored log buffer is 50000.
buffer-size: Specifies the size for the EAA-monitored log buffer, in the range of 1 to 500000.
After you execute a Syslog event monitor policy, the system saves a copy of the logs to the EAA-monitored log buffer. When the logs in the buffer match the Syslog event, EAA executes the monitor policy actions.
Typically, the default EAA-monitored log buffer size is sufficient. However, when a feature malfunctions or the user enables multiple debugging functions, a large number of logs are generated. Some logs might be discarded before the matching is performed. You can set the EAA-monitored log buffer to a large size based on the memory usage.
# Set the size of the EAA-monitored log buffer to 1000.
[Sysname] rtm event syslog buffer-size 1000
event syslog
rtm scheduler suspend
Use rtm scheduler suspend to suspend all monitor policies, including CLI monitor policies and Tcl monitor policies.
Use undo rtm scheduler suspend to resume monitor policies.
You need to suspend the monitor policies under the following circumstances:
· The monitor policies are triggered frequently, affecting the system services and performance.
· The Tcl script of a policy needs to be revised.
After you execute this command, EAA will not execute the policies even if the trigger conditions are met.
This command does not suspend a running monitor policy until all its actions are executed.
# Suspend monitor policies.
[Sysname] rtm scheduler suspend
rtm tcl-policy
Use rtm tcl-policy to create a Tcl-defined policy and bind it to a Tcl script file.
Use undo rtm tcl-policy to delete a Tcl policy.
undo rtm tcl-policy policy-name
No Tcl policies exist.
policy-name: Specifies a policy name, a case-sensitive string of 1 to 63 characters.
tcl-filename: Specifies a .tcl script file name. The file name is case sensitive. You must ensure that the file is available on a storage medium of the device.
When you use this command to create a Tcl-defined policy, follow these guidelines:
This command both creates and enables the specified Tcl-defined monitor policy. To revise the Tcl script of a Tcl-defined policy, you must suspend all monitor policies first, and then resume the policies after you finish revising the script. The system cannot execute a Tcl-defined policy if you edit its Tcl script without suspending all monitor policies.
To bind a Tcl-defined policy to a different Tcl script file:
1. Execute the undo rtm tcl-policy command to delete the Tcl policy.
2. Create the Tcl policy again, and then bind it to the new Tcl script file.
You can assign the same policy name to a CLI-defined policy and a Tcl-defined policy. However, you cannot assign the same name to policies that are the same type.
# Create a Tcl policy and bind it to a Tcl script file.
[Sysname] rtm tcl-policy test test.tcl
running-time
Use running-time to configure the action runtime of a CLI-defined policy.
Use undo running-time to restore the default.
running-time time
undo running-time
The action runtime of a CLI-defined policy is 20 seconds.
time: Specifies the action runtime in the range of 0 to 31536000 seconds. If you specify 0, the policy runs its actions forever once the policy is triggered.
Operating mechanism
The action runtime limits the amount of time that the monitor policy runs its actions from the time it is triggered. When the runtime is reached, the system stops executing the actions even if the execution is not finished.
This setting prevents an incorrectly defined policy from running its actions permanently to occupy resources.
For the actions of a periodic event monitor policy to be executed completely, the action running time must be smaller than or equal to the interval configured for the periodic event.
# Set the action runtime to 60 seconds for CLI-defined policy test.
[Sysname-rtm-test] running-time 60
event period
user-role
Use user-role to assign a user role to a CLI-defined policy.
Use undo user-role to remove a user role from a CLI-defined policy.
user-role role-name
undo user-role role-name
A monitor policy contains user roles that its creator had at the time of policy creation.
role-name: Specifies a user role by its name, a case-sensitive string of 1 to 63 characters. You set this parameter to be the name of an existing user role, for example, network-admin or network-operator. To display existing user roles, execute the user-role ? command in CLI monitoring policy view. Additionally, you can set this parameter to a user role name that does not exist on the device. In this case, you must create it by using the role name role-name command and assign permissions to it. For more information, see RBAC configuration in Fundamentals Configuration Guide.
For EAA to execute an action in a monitor policy, you must assign the policy the user role that has access to the action-specific commands and resources. If EAA lacks access to an action-specific command or resource, EAA does not perform the action and all the subsequent actions.
For example, a monitor policy has four actions numbered from 1 to 4. The policy has user roles that are required for performing actions 1, 3, and 4, but it does not have the user role required for performing action 2. When the policy is triggered, EAA executes only action 1.
A monitor policy supports a maximum of 64 valid user roles. User roles added after this limit is reached do not take effect.
An EAA policy cannot have both the security-audit user role and any other user roles. Any previously assigned user roles are automatically removed when you assign the security-audit user role to the policy. The previously assigned security-audit user role is automatically removed when you assign any other user roles to the policy.
# Assign user roles to a CLI-defined policy.
[Sysname-rtm-test] user-role admin