| 01-Text | 218.76 KB |
1 About the DPS-2400EB B power supply
IMPORTANT: · The information in this document might differ from your product if it contains custom configuration options or features. · The figures in this document are for illustration only. · For servers that support the DPS-2400EB B power supply, contact H3C Support. · The model name of a hardware option in this document might differ slightly from its model name label. A model name label might add a prefix or suffix to the hardware-coded model name. For example, the DPS-2400EB B power supply model represents power supply labels including UN-DPS-2400EB B, which has a different prefix. |
The DPS-2400EB B is an AC or high-voltage DC input and DC output power supply. It provides a maximum rated output of 2400 W.
Table1-1 DPS-2400EB B power supply description
Item |
Product code |
UN-DPS-2400EB B |
Detailed description |
2400W AC & 240V HVDC Power Supply Module (DT-R1-Platinum)(CTO&BTO) |
Sales code |
0231AFQB |
Lowest-level code |
0213A087 |
Figure1-1 DPS-2400EB B power supply
Figure1-2 Front panel
(1) LED |
(2) Latch |
(3) Power receptacle |
(4) Handle |
2 Key features
Protection
The power supply provides protection against input overcurrent, input undervoltage, output overvoltage, output overcurrent, output short circuit, and overtemperature conditions.
Redundancy
Multiple power supplies can be connected in parallel to achieve N+1 or N+N redundancy and load balancing.
Hot swapping
You can install or remove a power supply when the device is operating.
Tool-free replacement
You can replace a power supply without using tools.
3 Technical specifications
Table3-1 Technical specifications
Item |
Specifications |
Rated input voltage range |
· 100 VAC to 127 VAC @ 1000 W · 180 VAC to 200 VAC @ 2196 W · 200 VAC to 240 VAC @ 2400 W · 192 VAC to 210 VDC @ 1980 W · 210 VDC to 220 VDC @ 2196 W · 220 VDC to 288 VDC @ 2400 W |
Rated input current |
· 12.5 A MAX @ 100 VAC to 127 VAC · 14.5 A MAX @ 180 VAC to 200 VAC · 14.5 A MAX @ 200 VAC to 240 VAC · 13 A MAX @ 192 VDC to 210 VDC · 12 A MAX @ 210 VDC to 220 VDC · 12 A MAX @ 240 VDC |
Maximum rated heat dissipation |
· 4031 BTU/hr @ 100 VAC · 8959 BTU/hr @ 220 VAC · 8930 BTU/hr @ 240 VAC · 8948 BTU/hr @ 240 VDC · 8908 BTU/hr @ 270 VDC |
Maximum rated output power |
2400 W |
Rated output voltage |
· 12 V main circuit · 12 V auxiliary circuit |
Frequency |
50/60 Hz @ 100 VAC to 240 VAC |
Efficiency at 50% load |
80 Plus Platinum |
Temperature |
· Operating: 0°C to +55°C (32°F to 131°F) · Storage: –40°C to +70°C (–40°F to +158°F) |
Operating humidity |
5% to 85% |
Maximum altitude |
5000 m (16404.20 ft) |
Redundancy |
Yes |
Cold backup |
Yes |
4 LEDs
Table4-1 LED description
LED status |
Steady green |
The power supply is operating correctly. |
Flashing green (1 Hz) |
Power is being input correctly but the system is not powered on. |
Flashing green (0.33 Hz) |
The power supply is in standby state and is not outputting power. |
Flashing green (2 Hz) |
The power supply is updating its firmware. |
Steady amber |
· The power supply is faulty. · The power supply is not receiving power, but the other power supply is receiving power. |
Flashing amber (1 Hz) |
An alarm has occurred on the power supply. |
Off |
The power supply is not receiving power. Either or both of the following conditions might exist: · Power cord connection failure. · Power source shutdown. |
5 Installing and removing the power supply
For information about installing and removing the power supply, see the user guide for the device.