11-Network Management and Monitoring Configuration Guide
HomeSupportSwitchesS6520X-EI SeriesConfigure & DeployConfiguration GuidesH3C S6520X & S6520-SI & S5560X-HI & S5000-EI & MS4600 Configuration Guides-R6636Pxx-6W10111-Network Management and Monitoring Configuration Guide
20-Mirroring configuration
20-Mirroring configuration 547.36 KB
Configuring port mirroring· 1
About port mirroring· 1
Terminology· 1
Port mirroring classification· 2
Local port mirroring (SPAN) 2
Layer 2 remote port mirroring (RSPAN) 2
Layer 3 remote port mirroring (ERSPAN) 4
Restrictions and guidelines: Port mirroring configuration· 5
Configuring local port mirroring (SPAN) 5
Restrictions and guidelines for local port mirroring configuration· 5
Local port mirroring tasks at a glance· 6
Creating a local mirroring group· 6
Configuring mirroring sources· 6
Configuring the monitor port 6
Configuring local port mirroring group with multiple monitoring devices· 7
Configuring Layer 2 remote port mirroring (RSPAN) 8
Restrictions and guidelines for Layer 2 remote port mirroring configuration· 8
Layer 2 remote port mirroring with reflector port configuration task list 9
Layer 2 remote port mirroring with egress port configuration task list 9
Creating a remote destination group· 9
Configuring the monitor port 10
Configuring the remote probe VLAN· 10
Assigning the monitor port to the remote probe VLAN· 11
Creating a remote source group· 11
Configuring mirroring sources· 11
Configuring the reflector port 12
Configuring the egress port 13
Configuring Layer 3 remote port mirroring (ERSPAN in encapsulation parameter mode) 14
Restrictions and guidelines for Layer 3 remote port mirroring in ERSPAN mode configuration· 14
Layer 3 remote port mirroring tasks at a glance· 14
Creating a local mirroring group on the source device· 14
Configuring mirroring sources· 14
Configuring the monitor port 15
Display and maintenance commands for port mirroring· 16
Port mirroring configuration examples· 16
Example: Configuring local port mirroring(SPAN) 16
Example: Configuring local port mirroring with multiple monitoring devices· 17
Example: Configuring Layer 2 remote port mirroring (RSPAN with reflector port) 18
Example: Configuring Layer 2 remote port mirroring (RSPAN with egress port) 20
Example: Configuring Layer 3 remote port mirroring (ERSPAN in encapsulation parameter mode) 22
Configuring flow mirroring· 24
About flow mirroring· 24
Types of flow-mirroring traffic to an interface· 24
Flow mirroring SPAN or RSPAN· 24
Flow mirroring ERSPAN· 25
Restrictions and guidelines: Flow mirroring configuration· 27
Flow mirroring tasks at a glance· 27
Configuring a traffic class· 28
Configuring a traffic behavior 28
Configuring a QoS policy· 29
Applying a QoS policy· 29
Applying a QoS policy to an interface· 29
Applying a QoS policy to a VLAN· 30
Applying a QoS policy globally· 30
Display and maintenance commands for flow mirroring· 30
Flow mirroring configuration examples· 31
Example: Configuring flow mirroring· 31
Port mirroring copies the packets passing through a port to a port that connects to a data monitoring device for packet analysis.
Terminology
The following terms are used in port mirroring configuration.
Mirroring source
The mirroring sources can be one or more monitored ports called source ports.
Packets passing through mirroring sources are copied to a port connecting to a data monitoring device for packet analysis. The copies are called mirrored packets.
Source device
The device where the mirroring sources reside is called a source device.
Mirroring destination
The mirroring destination connects to a data monitoring device and is the destination port (also known as the monitor port) of mirrored packets. Mirrored packets are sent out of the monitor port to the data monitoring device.
A monitor port might receive multiple copies of a packet when it monitors multiple mirroring sources. For example, two copies of a packet are received on Port A when the following conditions exist:
·     Port A is monitoring bidirectional traffic of Port B and Port C on the same device.
·     The packet travels from Port B to Port C.
Destination device
The device where the monitor port resides is called the destination device.
Mirroring direction
The mirroring direction specifies the direction of the traffic that is copied on a mirroring source.
·     Inbound—Copies packets received.
·     Outbound—Copies packets sent.
·     Bidirectional—Copies packets received and sent.
Mirroring group
Port mirroring is implemented through mirroring groups. Mirroring groups can be classified into local mirroring groups, remote source groups, and remote destination groups.
Reflector port, egress port, and remote probe VLAN
Reflector ports, remote probe VLANs, and egress ports are used for Layer 2 remote port mirroring. The remote probe VLAN is a dedicated VLAN for transmitting mirrored packets to the destination device. Both the reflector port and egress port reside on a source device and send mirrored packets to the remote probe VLAN.
On port mirroring devices, all ports except source, destination, reflector, and egress ports are called common ports.
Port mirroring includes the following types:
·     Local port mirroringAlso known as Switch Port Analyzer (SPAN). In local port mirroring, the source device is directly connected to a data monitoring device. The source device acts as the destination device to forward mirrored packets to the data monitoring device.
·     Remote port mirroring—In remote port mirroring, the source device is not directly connected to a data monitoring device. The source device copies mirrored packets to the destination device, which forwards them to the data monitoring device. Depending on how the source device and the destination device are connected, remote port mirroring includes the following types:
¡     Layer 2 remote port mirroring—Also known as Remote SPAN (RSPAN). The source device and destination device are connected through a Layer 2 network.
¡     Layer 3 remote port mirroring—Also known as Encapsulated Remote SPAN (ERSPAN). The source device and destination device are connected through a Layer 3 network.
Figure 1 Local port mirroring implementation
As shown in Figure 1, the source port (Port A) and the monitor port (Port B) reside on the same device. Packets received on Port A are copied to Port B. Port B then forwards the packets to the data monitoring device for analysis.
In Layer 2 remote port mirroring, the mirroring sources and destination reside on different devices and are in different mirroring groups.
A remote source group is a mirroring group that contains the mirroring sources. A remote destination group is a mirroring group that contains the mirroring destination. Intermediate devices are the devices between the source device and the destination device.
Layer 2 remote port mirroring can be implemented through the reflector port method or the egress port method.
Reflector port method
In Layer 2 remote port mirroring that uses the reflector port method, packets are mirrored as follows:
1.     The source device copies packets received on the mirroring sources to the reflector port.
2.     The reflector port broadcasts the mirrored packets in the remote probe VLAN.
3.     The intermediate devices transmit the mirrored packets to the destination device through the remote probe VLAN.
4.     Upon receiving the mirrored packets, the destination device determines whether the ID of the mirrored packets is the same as the remote probe VLAN ID. If the two VLAN IDs match, the destination device forwards the mirrored packets to the data monitoring device through the monitor port.
Figure 2 Layer 2 remote port mirroring implementation through the reflector port method
Egress port method
In Layer 2 remote port mirroring that uses the egress port method, packets are mirrored as follows:
1.     The source device copies packets received on the mirroring sources to the egress port.
2.     The egress port forwards the mirrored packets to the intermediate devices.
3.     The intermediate devices flood the mirrored packets in the remote probe VLAN and transmit the mirrored packets to the destination device.
Figure 3 Layer 2 remote port mirroring implementation through the egress port method
Layer 3 remote port mirroring encapsulates mirrored packets in GRE packets with a protocol number of 0x88BE and routes the packets to the remote monitoring device.
The switch series supports implementing Layer 3 remote port mirroring in encapsulation parameter mode.
To implement Layer 3 remote port mirroring in encapsulation parameter mode, perform the following tasks:
1.     On the source device, create a local mirroring group and configure the mirroring sources, the monitor port, and the encapsulation parameters for mirrored packets.
2.     On all devices from source to destination, configure a unicast routing protocol to ensure Layer 3 reachability between the devices.
Create a local mirroring group on the source device, and specify the source ports and monitor port for the local mirroring group. When configuring the monitor port, specify the following encapsulation parameters for mirrored packets:
·     Monitoring device IP address as destination IP address.
·     Monitor port IP address as source IP address.
As shown in Figure 4, Layer 3 remote port mirroring in encapsulation parameter mode works as follows:
1.     The source device copies a packet passing through a source port.
2.     The source device encapsulates the copied packet with the specified encapsulation parameters, monitoring device IP as destination IP and monitor port IP as source IP.
3.     The encapsulated packet is routed to the monitoring device through the IP network.
4.     The monitoring device decapsulates the packet and analyzes the packet contents.
The packet sent to the monitoring device through Layer 3 remote port mirroring in encapsulation parameter mode is encapsulated. In this mode, make sure the monitoring device supports decapsulating packets.
Figure 4 Layer 3 remote port mirroring in encapsulation parameter mode
The reflector port method for Layer 2 remote port mirroring can be used to implement local port mirroring with multiple data monitoring devices.
In the reflector port method, the reflector port broadcasts mirrored packets in the remote probe VLAN. By assigning the ports that connect to data monitoring devices to the remote probe VLAN, you can implement local port mirroring to mirror packets to multiple data monitoring devices. The egress port method cannot implement local port mirroring in this way.
For inbound traffic mirroring, the VLAN tag in the original packet is copied to the mirrored packet.
For outbound traffic mirroring, the mirrored packet carries the VLAN tag of the egress interface.
Port mirroring and flow mirroring are mutually exclusive on the same port. If you first configure port mirroring and then configure flow mirroring on a port, only port mirroring takes effect. If you first configure flow mirroring and then port mirroring on a port, flow mirroring first takes effect, and port mirroring takes effect on packets that do not match flow mirroring.
A local mirroring group takes effect only after it is configured with the monitor port and mirroring sources.
A Layer 2 or Layer 3 aggregate interface, tunnel interface, or VLAN interface cannot be configured as a source port of a local mirroring group. You can configure member ports of a Layer 2 or Layer 3 aggregate interface as mirroring source ports.
A Layer 2 or Layer 3 aggregate interface cannot be configured as the monitor port of a local mirroring group.
The member port of an aggregate interface cannot be configured as a monitor port.
To configure local port mirroring, perform the following tasks:
1.     Configuring mirroring sources
2.     Configuring the monitor port
2.     Create a local mirroring group.
mirroring-group group-id local
Restrictions and guidelines for mirroring source configuration
When you configure source ports for a local mirroring group, follow these restrictions and guidelines:
·     A mirroring group can contain multiple source ports.
·     A port can act as a source port for only one mirroring group.
·     A source port cannot be configured as a reflector port, egress port, or monitor port.
·     A Layer 2 or Layer 3 aggregate interface, tunnel interface, or VLAN interface cannot be configured as a source port for a local mirroring group.
Configuring source ports
·     Configure source ports in system view:
a.     Enter system view.
b.     Configure source ports for a local mirroring group.
mirroring-group group-id mirroring-port interface-list { both | inbound | outbound }
By default, no source port is configured for a local mirroring group.
·     Configure source ports in interface view:
b.     Enter interface view.
c.     Configure the port as a source port for a local mirroring group.
mirroring-group group-id mirroring-port { both | inbound | outbound }
By default, a port does not act as a source port for any local mirroring groups.
Do not enable the spanning tree feature on the monitor port.
Only one monitor port can be specified for a local mirroring group.
Use a monitor port only for port mirroring, so the data monitoring device receives only the mirrored traffic.
The destination port cannot be any member port of an aggregate group.
·     Configure the monitor port in system view:
b.     Configure the monitor port for a local mirroring group.
mirroring-group group-id monitor-port interface-type interface-number
By default, no monitor port is configured for a local mirroring group.
·     Configure the monitor port in interface view:
c.     Configure the port as the monitor port for a mirroring group.
By default, a port does not act as the monitor port for any local mirroring groups.
About local port mirroring with multiple monitoring devices
To monitor interesting traffic passing through a device on multiple directly connected data monitoring devices, configure local port mirroring with a remote probe VLAN as follows:
1.     Configure a remote source group on the device.
2.     Configure mirroring sources and a reflector port for the remote source group.
3.     Specify a VLAN as the remote probe VLAN and assign the ports connecting to the data monitoring devices to the VLAN.
This configuration enables the device to copy packets received on the mirroring sources to the reflector port, which broadcasts the packets in the remote probe VLAN. The packets are then sent out of the member ports of the remote probe VLAN to the data monitoring devices.
The reflector port must be a port not in use. Do not connect a network cable to the reflector port.
When a port is configured as a reflector port, the port restores to the factory default settings. You cannot configure other features on the reflector port.
Do not assign a source port of a mirroring group to the remote probe VLAN of the mirroring group.
A VLAN can act as the remote probe VLAN for only one remote source group. As a best practice, use the VLAN for port mirroring exclusively. Do not create a VLAN interface for the VLAN or configure other features for the VLAN.
The remote probe VLAN must be a static VLAN.
To delete a VLAN that has been configured as the remote probe VLAN for a mirroring group, remove the remote probe VLAN from the mirroring group first.
The device supports only one remote probe VLAN.
2.     Create a remote source group.
mirroring-group group-id remote-source
3.     Configure mirroring sources for the remote source group. Choose one option as needed:
¡     Configure mirroring ports in system view.
¡     Execute the following commands in sequence to enter interface view and then configure the interface as a source port.
4.     Configure the reflector port for the remote source group.
mirroring-group group-id reflector-port reflector-port
By default, no reflector port is configured for a remote source group.
5.     Create a VLAN and enter its view.
vlan vlan-id
6.     Assign the ports that connect to the data monitoring devices to the VLAN.
port interface-list
By default, a VLAN does not contain any ports.
7.     Return to system view.
8.     Specify the VLAN as the remote probe VLAN for the remote source group.
mirroring-group group-id remote-probe vlan vlan-id
By default, no remote probe VLAN is configured for a remote source group.
To ensure successful traffic mirroring, configure devices in the order of the destination device, the intermediate devices, and the source device.
If intermediate devices exist, configure the intermediate devices to allow the remote probe VLAN to pass through.
For a mirrored packet to successfully arrive at the remote destination device, make sure its VLAN ID is not removed or changed.
Do not configure both MVRP and Layer 2 remote port mirroring. Otherwise, MVRP might register the remote probe VLAN with incorrect ports, which would cause the monitor port to receive undesired copies. For more information about MVRP, see Layer 2—LAN Switching Configuration Guide.
To monitor the bidirectional traffic of a source port, disable MAC address learning for the remote probe VLAN on the source, intermediate, and destination devices. For more information about MAC address learning, see Layer 2—LAN Switching Configuration Guide.
The member port of a Layer 2 or Layer 3 aggregate interface cannot be configured as the monitor port for Layer 2 remote port mirroring.
Configuring the destination device
1.     Creating a remote destination group
3.     Configuring the remote probe VLAN
4.     Assigning the monitor port to the remote probe VLAN
Configuring the source device
1.     Creating a remote source group
2.     Configuring mirroring sources
3.     Configuring the reflector port
4.     Configuring the remote probe VLAN
3.     Configuring the egress port
Perform this task on the destination device only.
2.     Create a remote destination group.
mirroring-group group-id remote-destination
Restrictions and guidelines for monitor port configuration
A monitor port can belong to only one mirroring group.
A Layer 2 or Layer 3 aggregate interface cannot be configured as the monitor port for a mirroring group.
Configuring the monitor port in system view
2.     Configure the monitor port for a remote destination group.
By default, no monitor port is configured for a remote destination group.
Configuring the monitor port in interface view
2.     Enter interface view.
3.     Configure the port as the monitor port for a remote destination group.
By default, a port does not act as the monitor port for any remote destination groups.
This task is required on the both the source and destination devices.
Only an existing static VLAN can be configured as a remote probe VLAN.
When a VLAN is configured as a remote probe VLAN, use the remote probe VLAN for port mirroring exclusively.
Configure the same remote probe VLAN for the remote source group and the remote destination group.
2.     Configure the remote probe VLAN for the remote source or destination group.
By default, no remote probe VLAN is configured for a remote source or destination group.
2.     Enter the interface view of the monitor port.
3.     Assign the port to the remote probe VLAN.
¡     Assign an access port to the remote probe VLAN.
port access vlan vlan-id
¡     Assign a trunk port to the remote probe VLAN.
port trunk permit vlan vlan-id
¡     Assign a hybrid port to the remote probe VLAN.
port hybrid vlan vlan-id { tagged | untagged }
For more information about the port access vlan, port trunk permit vlan, and port hybrid vlan commands, see Layer 2—LAN Switching Command Reference.
Perform this task on the source device only.
When you configure source ports for a remote source group, follow these restrictions and guidelines:
·     Do not assign a source port of a mirroring group to the remote probe VLAN of the mirroring group.
·     A source port cannot be configured as a reflector port, monitor port, or egress port.
b.     Configure source ports for a remote source group.
By default, no source port is configured for a remote source group.
c.     Configure the port as a source port for a remote source group.
By default, a port does not act as a source port for any remote source groups.
Restrictions and guidelines for reflector port configuration
A remote source group supports only one reflector port.
Configuring the reflector port in system view
2.     Configure the reflector port for a remote source group.
mirroring-group group-id reflector-port interface-type interface-number
CAUTION
CAUTION:
·     The port to be configured as a reflector port must be a port not in use. Do not connect a network cable to a reflector port.
·     When a port is configured as a reflector port, the default settings of the port are automatically restored. You cannot configure other features on the reflector port.
·     If an IRF port is bound to only one physical interface, do not configure the physical interface as a reflector port. Otherwise, the IRF might split.
Configuring the reflector port in interface view
CAUTION
CAUTION:
3.     Configure the port as the reflector port for a remote source group.
By default, a port does not act as the reflector port for any remote source groups.
Restrictions and guidelines for egress port configuration
Disable the following features on the egress port:
·     Spanning tree.
·     802.1X.
·     IGMP snooping.
·     Static ARP.
·     MAC address learning.
A port of an existing mirroring group cannot be configured as an egress port.
A mirroring group supports only one egress port.
Configuring the egress port in system view
2.     Configure the egress port for a remote source group.
mirroring-group group-id monitor-egress interface-type interface-number
By default, no egress port is configured for a remote source group.
3.     Enter the egress port view.
4.     Assign the egress port to the remote probe VLAN.
For more information about the port trunk permit vlan and port hybrid vlan commands, see Layer 2—LAN Switching Command Reference.
Configuring the egress port in interface view
3.     Configure the port as the egress port for a remote source group.
By default, a port does not act as the egress port for any remote source groups.
To implement ERSPAN in encapsulation parameter mode, perform the following tasks:
1.     On the source device, create a local mirroring group and configure the source ports, the monitor port, and the encapsulation parameters for mirrored packets.
For ERSPAN in encapsulation parameter mode, the data monitoring device must be able to remove the outer headers to obtain the original mirrored packets for analysis.
To configure Layer 3 remote port mirroring in ERSPAN mode, perform the following tasks:
1.     Creating a local mirroring group on the source device
3.     Configuring the monitor port
By default, no local mirroring group exists.
When you configure source ports for the local mirroring group, follow these restrictions and guidelines:
·     A port can act as a source port for only one mirroring group either as a unidirectional port or bidirectional port.
mirroring-group group-id mirroring-port interface-list inbound
mirroring-group group-id mirroring-port  inbound
An aggregation group member port cannot be configured as the monitor port for a mirroring group.
b.     Configure the monitor port in a local mirroring group and specify the encapsulation parameters.
mirroring-group group-id monitor-port interface-list destination-ip destination-ip-address source-ip source-ip-address [ dscp dscp-value | vlan vlan-id | vrf-instance vrf-name ] *
c.     Specify the port as the monitor port in a local mirroring group and configure the encapsulation parameters in a local mirroring group.
mirroring-group group-id monitor-port destination-ip destination-ip-address source-ip source-ip-address [ dscp dscp-value | vlan vlan-id | vrf-instance vrf-name ] *
Display mirroring group information.
display mirroring-group { group-id | all | local | remote-destination | remote-source }
As shown in Figure 5, configure local port mirroring in source port mode to enable the server to monitor the bidirectional traffic of the two departments.
Figure 5 Network diagram
# Create local mirroring group 1.
[Device] mirroring-group 1 local
# Configure Ten-GigabitEthernet 1/0/1 and Ten-GigabitEthernet 1/0/2 as source ports for local mirroring group 1.
[Device] mirroring-group 1 mirroring-port ten-gigabitethernet 1/0/1 ten-gigabitethernet 1/0/2 both
# Configure Ten-GigabitEthernet 1/0/3 as the monitor port for local mirroring group 1.
[Device] mirroring-group 1 monitor-port ten-gigabitethernet 1/0/3
# Disable the spanning tree feature on the monitor port (Ten-GigabitEthernet 1/0/3).
[Device] interface ten-gigabitethernet 1/0/3
[Device-Ten-GigabitEthernet1/0/3] undo stp enable
[Device-Ten-GigabitEthernet1/0/3] quit
# Verify the mirroring group configuration.
[Device] display mirroring-group all
Mirroring group 1:
    Type: Local
    Status: Active
    Mirroring port:
        Ten-GigabitEthernet1/0/1  Both
        Ten-GigabitEthernet1/0/2  Both
    Monitor port: Ten-GigabitEthernet1/0/3
As shown in Figure 6, Dept. A, Dept. B, and Dept. C are connected to the device through Ten-GigabitEthernet 1/0/1, Ten-GigabitEthernet 1/0/2, and Ten-GigabitEthernet 1/0/3, respectively.
Configure port mirroring to enable data monitoring devices Server A and Server B to monitor both the incoming and outgoing traffic of departments A, B, and C.
Figure 6 Network diagram
# Create remote source group 1.
[Device] mirroring-group 1 remote-source
# Configure Ten-GigabitEthernet 1/0/1 through Ten-GigabitEthernet 1/0/3 as source ports of remote source group 1.
[Device] mirroring-group 1 mirroring-port Ten-GigabitEthernet1/0/1 to Ten-GigabitEthernet1/0/3 both
# Configure an unused port (Ten-GigabitEthernet 1/0/6 in this example) as the reflector port of remote source group 1.
[Device] mirroring-group 1 reflector-port Ten-GigabitEthernet1/0/6
This operation may delete all settings made on the interface. Continue? [Y/N]:y
# Create VLAN 10 and assign the ports connecting the data monitoring devices to the VLAN.
[Device] vlan 10
[Device-vlan10] port Ten-GigabitEthernet1/0/4 to Ten-GigabitEthernet1/0/5
[Device-vlan10] quit
# Configure VLAN 10 as the remote probe VLAN of remote source group 1.
[Device] mirroring-group 1 remote-probe vlan 10
As shown in Figure 7, configure Layer 2 remote port mirroring to enable the server to monitor the bidirectional traffic of the Marketing Department.
Figure 7 Network diagram
1.     Configure Device C (the destination device):
# Configure Ten-GigabitEthernet 1/0/1 as a trunk port, and assign the port to VLAN 2.
<DeviceC> system-view
[DeviceC] interface ten-gigabitethernet 1/0/1
[DeviceC-Ten-GigabitEthernet1/0/1] port link-type trunk
[DeviceC-Ten-GigabitEthernet1/0/1] port trunk permit vlan 2
[DeviceC-Ten-GigabitEthernet1/0/1] quit
# Create a remote destination group.
[DeviceC] mirroring-group 2 remote-destination
# Create VLAN 2.
[DeviceC] vlan 2
# Disable MAC address learning for VLAN 2.
[DeviceC-vlan2] undo mac-address mac-learning enable
[DeviceC-vlan2] quit
# Configure VLAN 2 as the remote probe VLAN for the mirroring group.
[DeviceC] mirroring-group 2 remote-probe vlan 2
# Configure Ten-GigabitEthernet 1/0/2 as the monitor port for the mirroring group.
[DeviceC] interface ten-gigabitethernet 1/0/2
[DeviceC-Ten-GigabitEthernet1/0/2] mirroring-group 2 monitor-port
# Disable the spanning tree feature on Ten-GigabitEthernet 1/0/2.
[DeviceC-Ten-GigabitEthernet1/0/2] undo stp enable
# Assign Ten-GigabitEthernet 1/0/2 to VLAN 2.
[DeviceC-Ten-GigabitEthernet1/0/2] port access vlan 2
[DeviceC-Ten-GigabitEthernet1/0/2] quit
2.     Configure Device B (the intermediate device):
# Create VLAN 2.
[DeviceB] vlan 2
[DeviceB-vlan2] undo mac-address mac-learning enable
[DeviceB-vlan2] quit
[DeviceB-Ten-GigabitEthernet1/0/1] port link-type trunk
[DeviceB-Ten-GigabitEthernet1/0/1] port trunk permit vlan 2
# Configure Ten-GigabitEthernet 1/0/2 as a trunk port, and assign the port to VLAN 2.
[DeviceB] interface ten-gigabitethernet 1/0/2
[DeviceB-Ten-GigabitEthernet1/0/2] port link-type trunk
[DeviceB-Ten-GigabitEthernet1/0/2] port trunk permit vlan 2
[DeviceB-Ten-GigabitEthernet1/0/2] quit
3.     Configure Device A (the source device):
# Create a remote source group.
[DeviceA] mirroring-group 1 remote-source
# Create VLAN 2.
[DeviceA] vlan 2
[DeviceA-vlan2] undo mac-address mac-learning enable
[DeviceA-vlan2] quit
[DeviceA] mirroring-group 1 remote-probe vlan 2
# Configure Ten-GigabitEthernet 1/0/1 as a source port for the mirroring group.
[DeviceA] mirroring-group 1 mirroring-port ten-gigabitethernet 1/0/1 both
# Configure Ten-GigabitEthernet 1/0/3 as the reflector port for the mirroring group.
[DeviceA] mirroring-group 1 reflector-port ten-gigabitethernet 1/0/3
[DeviceA] interface ten-gigabitethernet 1/0/2
[DeviceA-Ten-GigabitEthernet1/0/2] port link-type trunk
[DeviceA-Ten-GigabitEthernet1/0/2] port trunk permit vlan 2
[DeviceA-Ten-GigabitEthernet1/0/2] quit
# Verify the mirroring group configuration on Device C.
[DeviceC] display mirroring-group all
Mirroring group 2:
    Type: Remote destination
    Status: Active
    Monitor port: Ten-GigabitEthernet1/0/2
    Remote probe VLAN: 2
# Verify the mirroring group configuration on Device A.
[DeviceA] display mirroring-group all
Mirroring group 1:
    Type: Remote source
    Status: Active
    Mirroring port:
    Reflector port: Ten-GigabitEthernet1/0/3
On the Layer 2 network shown in Figure 8, configure Layer 2 remote port mirroring to enable the server to monitor the bidirectional traffic of the Marketing Department.
Figure 8 Network diagram
# Create VLAN 2.
[DeviceC] vlan 2
# Assign Ten-GigabitEthernet 1/0/2 to VLAN 2 as an access port.
# Create VLAN 2.
[DeviceB] vlan 2
# Create VLAN 2.
[DeviceA] vlan 2
# Configure VLAN 2 as the remote probe VLAN of the mirroring group.
# Configure Ten-GigabitEthernet 1/0/2 as the egress port for the mirroring group.
[DeviceA] mirroring-group 1 monitor-egress ten-gigabitethernet 1/0/2
# Disable the spanning tree feature on the port.
[DeviceA-Ten-GigabitEthernet1/0/2] undo stp enable
Mirroring group 2:
    Status: Active
Mirroring group 1:
    Type: Remote source
    Status: Active
    Mirroring port:
    Monitor egress port: Ten-GigabitEthernet1/0/2
On a Layer 3 network shown in Figure 9, configure Layer 3 remote port mirroring in encapsulation parameter mode to enable the server to monitor the incoming traffic of the Marketing Department.
Figure 9 Network diagram
1.     Configure IP addresses for the interfaces as shown in Figure 9. (Details not shown.)
2.     Configure Device A (the source device):
# Enable the OSPF protocol.
[DeviceA] ospf 1
[DeviceA-ospf-1] area 0
[DeviceA-ospf-1-area-0.0.0.0] network 10.1.1.0 0.0.0.255
[DeviceA-ospf-1-area-0.0.0.0] network 20.1.1.0 0.0.0.255
[DeviceA-ospf-1-area-0.0.0.0] quit
[DeviceA-ospf-1] quit
[DeviceA] mirroring-group 1 local
# Configure Ten-GigabitEthernet 1/0/1 as a source port.
[DeviceA] mirroring-group 1 mirroring-port ten-gigabitethernet 1/0/1 inbound
# Configure Ten-GigabitEthernet 1/0/2 as the monitor port. Specify the destination and source IP addresses for mirrored packets as 40.1.1.2 and 20.1.1.1, respectively.
[DeviceA] mirroring-group 1 monitor-port ten-gigabitethernet 1/0/2 destination-ip 40.1.1.2 source-ip 20.1.1.1
3.     Enable the OSPF protocol on Device B.
[DeviceB] ospf 1
[DeviceB-ospf-1] area 0
[DeviceB-ospf-1-area-0.0.0.0] network 20.1.1.0 0.0.0.255
[DeviceB-ospf-1-area-0.0.0.0] network 30.1.1.0 0.0.0.255
[DeviceB-ospf-1-area-0.0.0.0] quit
[DeviceB-ospf-1] quit
4.     Enable the OSPF protocol on Device C.
[DeviceC] ospf 1
[DeviceC-ospf-1] area 0
[DeviceC-ospf-1-area-0.0.0.0] network 30.1.1.0 0.0.0.255
[DeviceC-ospf-1-area-0.0.0.0] network 40.1.1.0 0.0.0.255
[DeviceC-ospf-1-area-0.0.0.0] quit
[DeviceC-ospf-1] quit
Mirroring group 1:
    Type: Local
    Status: Active
    Mirroring port:
        Ten-GigabitEthernet1/0/1  Inbound
                  Encapsulation: Destination IP address 40.1.1.2
                                 Source IP address 20.1.1.1
                                 Destination MAC address 000f-e241-5e5b
Flow mirroring copies packets matching a class to a destination for packet analyzing and monitoring. It is implemented through QoS.
To implement flow mirroring through QoS, perform the following tasks:
·     Define traffic classes and configure match criteria to classify packets to be mirrored. Flow mirroring allows you to flexibly classify packets to be analyzed by defining match criteria.
·     Configure traffic behaviors to mirror the matching packets to the specified destination.
You can configure an action to mirror the matching packets to one of the following destinations:
·     Interface—The matching packets are copied to an interface and then forwarded to a data monitoring device for analysis.
·     Monitoring group—The matching packets are copied to the member interface of a monitoring group and then forwarded to the data monitoring devices directly connected to the interface.
·     CPU—The matching packets are copied to the CPU of an IRF member device. The CPU analyzes the packets or delivers them to upper layers.
For more information about QoS policies, traffic classes, and traffic behaviors, see ACL and QoS Configuration Guide.
Depending on whether the mirroring source and mirroring destination are on the same device, flow-mirroring traffic to an interface includes the following types:
·     Flow mirroring SPAN—Flow-mirrors traffic to a local interface.
·     Flow mirroring RSPAN—Flow-mirrors traffic to an interface, and then forwards traffic to a remote Layer 2 interface based on the VLAN of the mirrored traffic or through QoS traffic redirecting.
·     Flow mirroring ERSPAN—Encapsulates traffic in GRE packets with protocol number 0x88BE and routes the traffic to a remote monitoring device at Layer 3.
For flow mirroring SPAN, configure a QoS policy on the source device. Configure the QoS policy as follows:
1.     Configure a traffic class to match packets.
2.     Configure a traffic behavior to flow-mirror traffic to an interface.
3.     Associate the traffic class with the traffic behavior.
When the device receives a matching packet, the device sends one copy of the packet to the interface specified by the traffic behavior. The interface forwards the mirrored packet to the monitoring device.
Figure 10 Flow mirroring SPAN
To implement RSPAN, forward the mirrored packet to a remote Layer 2 interface based on the VLAN of the mirrored packet or through QoS traffic redirecting.
Flow mirroring ERSPAN can be implemented in monitoring group mode.
Encapsulation parameter mode
In this mode, configure a QoS policy on the source device. Configure the QoS policy as follows:
You can specify both the outgoing interface and encapsulation parameters when configuring flow-mirroring traffic to an interface. The device encapsulates packets with the specified parameters and then forwards packets out of the specified interface.
As shown in Figure 11, flow mirroring ERSPAN in encapsulation parameter mode works as follows:
1.     The source device copies a matching packet.
2.     The source device encapsulates the packet with the specified ERSPAN encapsulation parameters.
3.     The source device forwards the mirrored packets out of the specified outgoing interface.
4.     The encapsulated packet is routed to the monitoring device.
5.     The monitoring device decapsulates the packet and analyzes the packet contents.
The packet sent to the monitoring device through flow mirroring in this mode is encapsulated. In this mode, make sure the monitoring device supports decapsulating packets.
Figure 11 Flow mirroring ERSPAN in encapsulation parameter mode
Monitoring group mode
As shown in Figure 12, flow mirroring ERSPAN in monitoring group mode works as follows:
1.     On the source device, configure a monitoring group, add member interfaces to the monitoring group, and configure the encapsulation parameters for the member interfaces.
2.     On the source device, apply a QoS policy as follows:
a.     Configure a traffic class to match packets.
b.     Configure a traffic behavior to mirror traffic to the monitoring group.
c.     Create a QoS policy, and associate the traffic class with the traffic behavior in the QoS policy.
d.     Apply the QoS policy.
3.     The source device copies a matching packet and mirrors the packet to the monitoring group. The member interfaces of the monitoring group encapsulate the packet with the specified encapsulation parameters.
4.     The source device forwards the packet in either of the following methods:
¡     Forwards the mirrored packet out of the specified outgoing interface.
¡     Looks up a route for the encapsulated mirrored packet based on the source IP address and destination IP address of the encapsulated packet.
5.     The encapsulated packet is routed to the monitoring device.
6.     The monitoring device decapsulates the packet and analyzes the packet contents.
Figure 12 Flow mirroring ERSPAN in monitoring group mode
For information about the configuration commands except the mirror-to command, see ACL and QoS Command Reference.
To configure flow mirroring, perform the following tasks:
1.     Configuring a traffic class
A traffic class defines the criteria that filters the traffic to be mirrored.
2.     Configuring a traffic behavior
A traffic behavior specifies mirroring destinations.
3.     Configuring a QoS policy
4.     Applying a QoS policy
¡     Applying a QoS policy to an interface
¡     Applying a QoS policy to a VLAN
¡     Applying a QoS policy globally
2.     Create a class and enter class view.
3.     Configure match criteria.
if-match match-criteria
By default, no match criterion is configured in a traffic class.
4.     (Optional.) Display traffic class information.
For more information about this command, see ACL and QoS Command Reference.
2.     Configure a monitoring group.
a.     Create a monitoring group.
monitoring-group group-id
b.     Assign ports to the monitoring group.
Syntax I:
monitoring-port interface-list
By default, a monitoring group does not contain any port.
c.     Return to system view.
3.     Create a traffic behavior and enter traffic behavior view.
4.     Configure mirroring destinations for the traffic behavior. Choose one option as needed:
¡     Mirror traffic to interfaces.
Syntax I:
mirror-to interface interface-type interface-number
Syntax II:
mirror-to interface interface-type interface-number reflector-port interface-type interface-number strip-vlan vlan-id
When you use syntax II, the specified mirroring destination interface and reflector port must be assigned to a mirroring-type service loopback group. For more information about service loopback groups, see service loopback group configuration in Layer 2—LAN Switching Configuration Guide.
By default, no mirroring actions exist to mirror traffic to interfaces.
You can mirror traffic to only one interface in a traffic behavior. If you execute this command for a traffic behavior multiple times, only the most recent configuration takes effect.
¡     Mirror traffic to a monitoring group.
mirror-to monitoring-group group-id
By default, no mirroring actions exist to mirror traffic to a monitoring group.
¡     Mirror traffic to the CPU.
mirror-to cpu
By default, no mirroring actions exist to mirror traffic to the CPU.
5.     (Optional.) Display traffic behavior configuration.
2.     Create a QoS policy and enter QoS policy view.
qos mirroring policy policy-name
3.     Associate a class with a traffic behavior in the QoS policy.
classifier classifier-name behavior behavior-name
By default, no traffic behavior is associated with a class.
4.     (Optional.) Display QoS policy configuration.
display qos policy user-defined mirroring [ policy-name [ classifier classifier-name ] ] [ slot slot-number ]
You can apply a QoS policy to an interface to mirror the traffic of the interface.
A policy can be applied to multiple interfaces.
A QoS policy cannot be applied in the outbound direction of an interface. In the inbound direction of an interface, only one QoS policy can be applied.
3.     Apply a policy to the interface.
qos apply mirroring policy policy-name inbound
4.     (Optional.) Display the QoS policy applied to the interface.
display qos mirroring policy interface [ interface-type interface-number [ inbound | outbound ] [ slot slot-number ]
You can apply a QoS policy to a VLAN to mirror the traffic on all ports in the VLAN.
A QoS policy cannot be applied in the outbound direction of a VLAN. In the inbound direction of a VLAN, only one QoS policy can be applied.
2.     Apply a QoS policy to a VLAN.
qos vlan-policy policy-name vlan vlan-id-list inbound
3.     (Optional.) Display the QoS policy applied to the VLAN.
display qos vlan-policy { name policy-name | vlan [ vlan-id ] }inbound [ slot slot-number ]
You can apply a QoS policy globally to mirror the traffic on all ports.
A QoS policy cannot be applied in the outbound direction globally. In the inbound direction, only one QoS policy can be applied globally.
2.     Apply a QoS policy globally.
qos apply mirroring policy policy-name global inbound
3.     (Optional.) Display global QoS policies.
display qos mirroring policy global inbound [ slot slot-number ]
Display monitoring group information.
display monitoring-group { group-id | all }
As shown in Figure 13, configure flow mirroring so that the server can monitor the following traffic:
·     All traffic that the Technical Department sends to access the Internet.
·     IP traffic that the Technical Department sends to the Marketing Department during working hours (8:00 to 18:00) on weekdays.
Figure 13 Network diagram
# Create working hour range work, in which working hours are from 8:00 to 18:00 on weekdays.
[Device] time-range work 8:00 to 18:00 working-day
# Create IPv4 advanced ACL 3000 to allow packets from the Technical Department to access the Internet and the Marketing Department during working hours.
[Device] acl advanced 3000
[Device-acl-ipv4-adv-3000] rule permit tcp source 192.168.2.0 0.0.0.255 destination-port eq www
[Device-acl-ipv4-adv-3000] rule permit ip source 192.168.2.0 0.0.0.255 destination 192.168.1.0 0.0.0.255 time-range work
# Create traffic class tech_c, and configure the match criterion as ACL 3000.
[Device] traffic classifier tech_c
[Device-classifier-tech_c] if-match acl 3000
[Device-classifier-tech_c] quit
# Create traffic behavior tech_b, configure the action of mirroring traffic to Ten-GigabitEthernet 1/0/3.
[Device] traffic behavior tech_b
[Device-behavior-tech_b] mirror-to interface ten-gigabitethernet 1/0/3
[Device-behavior-tech_b] quit
# Create QoS policy tech_p, and associate traffic class tech_c with traffic behavior tech_b in the QoS policy.
[Device] qos policy tech_p
[Device-qospolicy-tech_p] classifier tech_c behavior tech_b
[Device-qospolicy-tech_p] quit
# Apply QoS policy tech_p to the incoming packets of Ten-GigabitEthernet 1/0/4.
[Device] interface ten-gigabitethernet 1/0/4
[Device-Ten-GigabitEthernet1/0/4] qos apply policy tech_p inbound
[Device-Ten-GigabitEthernet1/0/4] quit
# Verify that the server can monitor the following traffic:
·     All traffic sent by the Technical Department to access the Internet.
·     IP traffic that the Technical Department sends to the Marketing Department during working hours on weekdays.