- 11-Network Management and Monitoring Configuration Guide
- 02-NQA configuration
- 03-iNQA configuration
- 04-NTP configuration
- 05-PTP configuration
- 06-SNMP configuration
- 07-RMON configuration
- 08-Event MIB configuration
- 09-NETCONF configuration
- 10-Ansible configuration
- 11-Puppet configuration
- 12-Chef configuration
- 13-CWMP configuration
- 14-EAA configuration
- 15-Process monitoring and maintenance configuration
- 16-Mirroring configuration
- 17-sFlow configuration
- 18-Information center configuration
- 19-Packet capture configuration
- 20-VCF fabric configuration
- 21-eMDI configuration
- 22-SQA configuration
- 23-TCP connection trace configuration
| 09-NETCONF configuration | 446.95 KB |
Establishing a NETCONF session
Restrictions and guidelines for NETCONF session establishment
Setting NETCONF session attributes
Establishing NETCONF over SOAP sessions
Establishing NETCONF over SSH sessions
Establishing NETCONF over Telnet or NETCONF over console sessions
Retrieving device configuration information
Restrictions and guidelines for device configuration retrieval
Retrieving device configuration and state information
Retrieving non-default settings
Retrieving NETCONF information
Retrieving NETCONF session information
Example: Retrieving a data entry for the interface table
Example: Retrieving non-default configuration data
Example: Retrieving syslog configuration data
Example: Retrieving NETCONF session information
Restrictions and guidelines for data filtering
Example: Filtering data with regular expression match
Example: Filtering data by conditional match
Locking or unlocking the running configuration
About configuration locking and unlocking
Restrictions and guidelines for configuration locking and unlocking
Locking the running configuration
Unlocking the running configuration
Example: Locking the running configuration
About the <edit-config> operation
Example: Modifying the configuration
Saving the running configuration
Example: Saving the running configuration
Rolling back the configuration
Rolling back the configuration based on a configuration file
Rolling back the configuration based on a rollback point
Performing CLI operations through NETCONF
About CLI operations through NETCONF
Example: Performing CLI operations
Subscribing to events monitored by NETCONF
Subscribing to events reported by modules
Canceling an event subscription
Example: Subscribing to syslog events
About NETCONF session termination
Example: Terminating another NETCONF session
Enabling SNMP notifications for NETCONF
Display and maintenance commands for NETCONF
edit-config: default-operation
Configuring NETCONF
About NETCONF
Network Configuration Protocol (NETCONF) is an XML-based network management protocol. It provides programmable mechanisms to manage and configure network devices. Through NETCONF, you can configure device parameters, retrieve parameter values, and collect statistics. For a network that has devices from vendors, you can develop a NETCONF-based NMS system to configure and manage devices in a simple and effective way.
NETCONF structure
NETCONF has the following layers: content layer, operations layer, RPC layer, and transport protocol layer.
Table 1 NETCONF layers and XML layers
NETCONF layer |
XML layer |
Content |
Configuration data, status data, and statistics |
Contains a set of managed objects, which can be configuration data, status data, and statistics. For information about the operable data, see the NETCONF XML API reference for the device. |
Operations |
<get>, <get-config>, <edit-config>… |
Defines a set of base operations invoked as RPC methods with XML-encoded parameters. NETCONF base operations include data retrieval operations, configuration operations, lock operations, and session operations. For information about operations supported on the device, see "Supported NETCONF operations." |
RPC |
<rpc> and <rpc-reply> |
Provides a simple, transport-independent framing mechanism for encoding RPCs. The <rpc> and <rpc-reply> elements are used to enclose NETCONF requests and responses (data at the operations layer and the content layer). |
Transport protocol |
In non-FIPS mode: Console, Telnet, SSH, HTTP, HTTPS, and TLS In FIPS mode: Console, SSH, HTTPS, and TLS |
Provides reliable, connection-oriented, serial data links. The following transport layer sessions are available in non-FIPS mode: · CLI sessions, including NETCONF over Telnet sessions, NETCONF over SSH sessions, and NETCONF over console sessions. · NETCONF over SOAP sessions, including NETCONF over SOAP over HTTP sessions and NETCONF over SOAP over HTTPS sessions. The following transport layer sessions are available in FIPS mode: · CLI sessions, including NETCONF over SSH sessions and NETCONF over console sessions. · NETCONF over SOAP over HTTPS sessions. |
NETCONF message format
NETCONF
All NETCONF messages are XML-based and comply with RFC 4741. An incoming NETCONF message must pass XML schema check before it can be processed. If a NETCONF message fails XML schema check, the device sends an error message to the client.
For information about the NETCONF operations supported by the device and the operable data, see the NETCONF XML API reference for the device.
The following example shows a NETCONF message for getting all parameters of all interfaces on the device:
<?xml version="1.0" encoding="utf-8"?>
<rpc message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0">
<get-bulk>
<filter type="subtree">
<top xmlns="http://www.h3c.com/netconf/data:1.0">
<Ifmgr>
<Interfaces>
<Interface/>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get-bulk>
</rpc>
NETCONF over SOAP
All NETCONF over SOAP messages are XML-based and comply with RFC 4741. NETCONF messages are contained in the <Body> element of SOAP messages. NETCONF over SOAP messages also comply with the following rules:
· SOAP messages must use the SOAP Envelope namespaces.
· SOAP messages must use the SOAP Encoding namespaces.
· SOAP messages cannot contain the following information:
¡ DTD reference.
¡ XML processing instructions.
The following example shows a NETCONF over SOAP message for getting all parameters of all interfaces on the device:
<env:Envelope xmlns:env="http://www.w3.org/2003/05/soap-envelope">
<env:Header>
<auth:Authentication env:mustUnderstand="1" xmlns:auth="http://www.h3c.com/netconf/base:1.0">
<auth:AuthInfo>800207F0120020C</auth:AuthInfo>
</auth:Authentication>
</env:Header>
<env:Body>
<get-bulk>
<Ifmgr>
<Interfaces>
<Interface/>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get-bulk>
</rpc>
</env:Body>
</env:Envelope>
How to use NETCONF
You can use NETCONF to manage and configure the device by using the methods in Table 2.
Table 2 NETCONF methods for configuring the device
Configuration tool |
Login method |
Remarks |
CLI |
· Console port · SSH · Telnet |
To perform NETCONF operations, copy valid NETCONF messages to the CLI in XML view. |
Custom user interface |
N/A |
This method requires a NETCONF over SOAP session or NETCONF over SSH session with the device. To use a NETCONF over SOAP session, you must enable NETCONF over SOAP. Then, NETCONF messages will be encapsulated in SOAP messages for transmission. |
Protocols and standards
· RFC 3339, Date and Time on the Internet: Timestamps
· RFC 4741, NETCONF Configuration Protocol
· RFC 4742, Using the NETCONF Configuration Protocol over Secure SHell (SSH)
· RFC 4743, Using NETCONF over the Simple Object Access Protocol (SOAP)
· RFC 5277, NETCONF Event Notifications
· RFC 5381, Experience of Implementing NETCONF over SOAP
· RFC 5539, NETCONF over Transport Layer Security (TLS)
· RFC 6241, Network Configuration Protocol
FIPS compliance
The device supports the FIPS mode that complies with NIST FIPS 140-2 requirements. Support for features, commands, and parameters might differ in FIPS mode (see Security Configuration Guide) and non-FIPS mode.
NETCONF tasks at a glance
To configure NETCONF, perform the following tasks:
1. Establishing a NETCONF session
a. (Optional.) Setting NETCONF session attributes
b. Establishing NETCONF over SOAP sessions
c. Establishing NETCONF over SSH sessions
d. Establishing NETCONF over Telnet or NETCONF over console sessions
2. (Optional.) Retrieving device configuration information
¡ Retrieving device configuration and state information
¡ Retrieving non-default settings
¡ Retrieving NETCONF information
¡ Retrieving YANG file content
¡ Retrieving NETCONF session information
3. (Optional.) Filtering data
4. (Optional.) Locking or unlocking the running configuration
a. Locking the running configuration
b. Unlocking the running configuration
5. (Optional.) Modifying the configuration
6. (Optional.) Managing configuration files
¡ Saving the running configuration
¡ Rolling back the configuration
7. (Optional.) Performing CLI operations through NETCONF
8. (Optional.) Subscribing to events
¡ Subscribing to syslog events
¡ Subscribing to events monitored by NETCONF
¡ Subscribing to events reported by modules
¡ Canceling an event subscription
9. (Optional.) Terminating NETCONF sessions
10. (Optional.) Returning to the CLI
11. (Optional.) Enabling SNMP notifications for NETCONF
After a NETCONF session is established, the device automatically sends its capabilities to the client. You must send the capabilities of the client to the device before you can perform any other NETCONF operations.
Before performing a NETCONF operation, make sure no other users are configuring or managing the device. If multiple users simultaneously configure or manage the device, the result might be different from what you expect.
You can use the aaa session-limit command to set the maximum number of NETCONF sessions that the device can support. If the upper limit is reached, new NETCONF users cannot access the device. For information about this command, see AAA in Security Configuration Guide.
NETCONF supports the following types of namespaces:
· Common namespace—The common namespace is shared by all modules. In a packet that uses the common namespace, the namespace is indicated in the <top> element, and the modules are listed under the <top> element.
Example:
<get-bulk>
<Ifmgr>
<Interfaces>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get-bulk>
</rpc>
· Module-specific namespace—Each module has its own namespace. A packet that uses a module-specific namespace does not have the <top> element. The namespace follows the module name.
Example:
<get-bulk>
<Ifmgr xmlns="http://www.h3c.com/netconf/data:1.0-Ifmgr">
<Interfaces>
</Interfaces>
</Ifmgr>
</filter>
</get-bulk>
</rpc>
The common namespace is incompatible with module-specific namespaces. To set up a NETCONF session, the device and the client must use the same type of namespaces. By default, the common namespace is used. If the client does not support the common namespace, use this feature to configure the device to use module-specific namespaces.
1. Enter system view.
2. Set the NETCONF session idle timeout time.
netconf { agent | soap } idle-timeout minute
Keyword |
agent |
Specifies the following sessions: · NETCONF over SSH sessions. · NETCONF over Telnet sessions. · NETCONF over console sessions. By default, the idle timeout time is 0, and the sessions never time out. |
soap |
Specifies the following sessions: · NETCONF over SOAP over HTTP sessions. · NETCONF over SOAP over HTTPS sessions. The default setting is 10 minutes. |
3. Enable NETCONF logging.
netconf log source { all | { agent | soap } * } { protocol-operation { all | { action | config | get | set | session | syntax | others } * } | row-operation | verbose }
By default, the device logs only row operations for <action> and <edit-config> operations. NETCONF logging is disabled for all the other types of operations.
4. Configure NETCONF to use module-specific namespaces.
netconf capability specific-namespace
For the setting to take effect, you must reestablish the NETCONF session.
You can use a custom user interface to establish a NETCONF over SOAP session to the device and perform NETCONF operations. NETCONF over SOAP encapsulates NETCONF messages into SOAP messages and transmits the SOAP messages over HTTP or HTTPS.
You can add an authentication domain to the <UserName> parameter of a SOAP request. The authentication domain takes effect only on the current request.
The mandatory authentication domain configured by using the netconf soap domain command takes precedence over the authentication domain specified in the <UserName> parameter of a SOAP request.
2. (Optional.) Apply an SSL server policy to the NETCONF over SOAP over HTTPS service.
netconf soap https ssl-server-policy policy-name
By default, no SSL server policy is applied to the NETCONF over SOAP over HTTPS service.
The NETCONF over SOAP over HTTPS service will use the SSL server policy to enhance service security. For more information about SSL server policies, see SSL configuration in Security Configuration Guide.
If you modify the applied SSL server policy after NETCONF over SOAP over HTTPS is enabled, the changes apply only to the NETCONF over SOAP over HTTPS sessions established subsequently. They do not take effect on the NETCONF over SOAP over HTTPS sessions that have been established before you modify the policy.
3. Enable NETCONF over SOAP.
In non-FIPS mode:
netconf soap { http | https } enable
In FIPS mode:
netconf soap https enable
By default, the NETCONF over SOAP feature is disabled.
4. (Optional.) Set the DSCP value for NETCONF over SOAP packets.
In non-FIPS mode:
netconf soap { http | https } dscp dscp-value
In FIPS mode:
netconf soap https dscp dscp-value
By default, the DSCP value is 0 for NETCONF over SOAP packets.
5. (Optional.) Use an IPv4 ACL to control NETCONF over SOAP access.
In non-FIPS mode:
netconf soap { http | https } acl { ipv4-acl-number | name ipv4-acl-name }
In FIPS mode:
netconf soap https acl { ipv4-acl-number | name ipv4-acl-name }
By default, no IPv4 ACL is applied to control NETCONF over SOAP access.
Only clients permitted by the IPv4 ACL can establish NETCONF over SOAP sessions.
6. (Optional.) Specify a mandatory authentication domain for NETCONF users.
netconf soap domain domain-name
By default, no mandatory authentication domain is specified for NETCONF users. For information about authentication domains, see Security Configuration Guide.
7. Use the custom user interface to establish a NETCONF over SOAP session with the device.
For information about the custom user interface, see the user guide for the interface.
Before establishing a NETCONF over SSH session, make sure the custom user interface can access the device through SSH.
2. Enable NETCONF over SSH.
netconf ssh server enable
By default, NETCONF over SSH is disabled.
3. Specify the listening port for NETCONF over SSH packets.
netconf ssh server port port-number
By default, the listening port number is 830.
4. Use the custom user interface to establish a NETCONF over SSH session with the device. For information about the custom user interface, see the user guide for the interface.
To ensure the format correctness of a NETCONF message, do not enter the message manually. Copy and paste the message.
While the device is performing a NETCONF operation, do not perform any other operations, such as pasting a NETCONF message or pressing Enter.
For the device to identify NETCONF messages, you must add end mark ]]>]]> at the end of each NETCONF message. Examples in this document do not necessarily have this end mark. Do add the end mark in actual operations.
To establish a NETCONF over Telnet session or a NETCONF over console session, first log in to the device through Telnet or the console port.
To enter XML view, execute the following command in user view:
xml
If the XML view prompt appears, the NETCONF over Telnet session or NETCONF over console session is established successfully.
Exchanging capabilities
After a NETCONF session is established, the device sends its capabilities to the client. You must use a hello message to send the capabilities of the client to the device before you can perform any other NETCONF operations.
Hello message from the device to the client
<?xml version="1.0" encoding="UTF-8"?><hello xmlns="urn:ietf:params:xml:ns:netconf:base:1.0"><capabilities>...</capabilities><session-id>1</session-id></hello>]]>]]>
The <capabilities> element carries the capabilities supported by the device. The supported capabilities vary by device model.
The <session-id> element carries the unique ID assigned to the NETCONF session.
Hello message from the client to the device
After receiving the hello message from the device, copy the following hello message to notify the device of the capabilities supported by the client:
<capabilities>
<capability>
capability-set
</capability>
</capabilities>
</hello>
Item |
capability-set |
Specifies a set of capabilities supported by the client. Use the <capability> and </capability> tags to enclose each user-defined capability set. |
As a best practice to ensure retrieval performance, limit the number of data entries for each <get-bulk> or <get> operation to 1000. If the number of data entries to retrieve is higher than 1000, use the <get-bulk> operation as a best practice.
During a <get>, <get-bulk>, <get-config>, or <get-bulk-config> operation, NETCONF replaces unidentifiable characters in the retrieved data with question marks (?) before sending the data to the client. If the process for a relevant module is not started yet, the operation returns the following message:
<?xml version="1.0"?>
<rpc-reply message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0">
<data/>
</rpc-reply>
The <get><netconf-state/></get> operation does not support data filtering.
For more information about the NETCONF operations, see the NETCONF XML API references for the device.
You can use the following NETCONF operations to retrieve device configuration and state information:
· <get> operation—Retrieves all device configuration and state information that matches the specified conditions.
· <get-bulk> operation—Retrieves data entries starting from the data entry next to the one with the specified index. One data entry contains a device configuration entry and a state information entry. The returned output does not include the index information.
The <get> message and <get-bulk> message share the following format:
<getoperation>
<filter>
Specify the module, submodule, table name, and column name
</top>
</filter>
</getoperation>
</rpc>
Item |
getoperation |
Operation name, get or get-bulk. |
filter |
Specifies the filtering conditions, such as the module name, submodule name, table name, and column name. · If you specify a module name, the operation retrieves the data for the specified module. If you do not specify a module name, the operation retrieves the data for all modules. · If you specify a submodule name, the operation retrieves the data for the specified submodule. If you do not specify a submodule name, the operation retrieves the data for all submodules. · If you specify a table name, the operation retrieves the data for the specified table. If you do not specify a table name, the operation retrieves the data for all tables. · If you specify only the index column, the operation retrieves the data for all columns. If you specify the index column and any other columns, the operation retrieves the data for the index column and the specified columns. |
A <get-bulk> message can carry the count and index attributes.
Item |
index |
Specifies the index. If you do not specify this item, the index value starts with 1 by default. |
count |
Specifies the data entry quantity. The count attribute complies with the following rules: · The count attribute can be placed in the module node and table node. In other nodes, it cannot be resolved. · When the count attribute is placed in the module node, a descendant node inherits this count attribute if the descendant node does not contain the count attribute. · The <get-bulk> operation retrieves all the rest data entries starting from the data entry next to the one with the specified index if either of the following conditions occurs: ¡ You do not specify the count attribute. ¡ The number of matching data entries is less than the value of the count attribute. |
The following <get-bulk> message example specifies the count and index attributes:
<rpc message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" xmlns:xc="http://www.h3c.com/netconf/base:1.0">
<get-bulk>
<top xmlns="http://www.h3c.com/netconf/data:1.0" xmlns:base="http://www.h3c.com/netconf/base:1.0">
<Syslog>
<Logs xc:count="5">
<Log>
<Index>10</Index>
</Log>
</Logs>
</Syslog>
</top>
</filter>
</get-bulk>
</rpc>
When retrieving interface information, the device cannot identify whether an integer value for the <IfIndex> element represents an interface name or index. When retrieving VPN instance information, the device cannot identify whether an integer value for the <vrfindex> element represents a VPN name or index. To resolve the issue, you can use the valuetype attribute to specify the value type.
The valuetype attribute has the following values:
Value |
name |
The element carries a name. |
index |
The element carried an index. |
auto |
Default value. The device uses the value of the element as an index for information matching. If no match is found, the device uses the value as a name for information matching. |
The following example specifies an index-type value for the <IfIndex> element:
<rpc xmlns="urn:ietf:params:xml:ns:netconf:base:1.0">
<getoperation>
<filter>
<top xmlns="http://www.h3c.com/netconf/config:1.0" xmlns:base="http://www.h3c.com/netconf/base:1.0">
<VLAN>
<TrunkInterfaces>
<Interface>
<IfIndex base:valuetype="index">1</IfIndex>
</Interface>
</TrunkInterfaces>
</VLAN>
</top>
</filter >
</getoperation>
</rpc>
If the <get> or < get-bulk> operation succeeds, the device returns the retrieved data in the following format:
<data>
Device state and configuration data
</data>
</rpc-reply>
The <get-config> and <get-bulk-config> operations are used to retrieve all non-default settings. The <get-config> and <get-bulk-config> messages can contain the <filter> element for filtering data.
The <get-config> and <get-bulk-config> messages are similar. The following is a <get-config> message example:
<get-config>
<source>
<running/>
</source>
<filter>
<top xmlns="http://www.h3c.com/netconf/config:1.0">
Specify the module name, submodule name, table name, and column name
</top>
</filter>
</get-config>
</rpc>
If the <get-config> or <get-bulk-config> operation succeeds, the device returns the retrieved data in the following format:
<data>
Data matching the specified filter
</data>
</rpc-reply>
Use the <get><netconf-state/></get> message to retrieve NETCONF information.
# Copy the following text to the client to retrieve NETCONF information:
<rpc message-id="m-641" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0">
<get>
<filter type='subtree'>
<netconf-state xmlns='urn:ietf:params:xml:ns:yang:ietf-netconf-monitoring'>
<getType/>
</netconf-state>
</filter>
</get>
</rpc>
If you do not specify a value for getType, the retrieval operation retrieves all NETCONF information.
The value for getType can be one of the following operations:
Operation |
capabilities |
Retrieves device capabilities. |
datastores |
Retrieves databases from the device. |
schemas |
Retrieves the list of the YANG file names from the device. |
sessions |
Retrieves session information from the device. |
statistics |
Retrieves NETCONF statistics. |
If the <get><netconf-state/></get> operation succeeds, the device returns a response in the following format:
<data>
Retrieved NETCONF information
</data>
</rpc-reply>
YANG files save the NETCONF operations supported by the device. You can identify the supported operations by retrieving and analyzing the content of YANG files.
YANG files are integrated in the device software and are named in the format of yang_identifier@yang_version.yang. You cannot view the YANG file names by executing the dir command. For information about retrieving the YANG file names, see "Retrieving NETCONF information."
# Copy the following text to the client to retrieve the YANG file named [email protected]:
<get-schema xmlns='urn:ietf:params:xml:ns:yang:ietf-netconf-monitoring'>
<identifier>H3C-syslog-data</identifier>
<version>2019-01-01</version>
<format>yang</format>
</get-schema>
</rpc>
If the <get-schema> operation succeeds, the device returns a response in the following format:
<data>
Content of the specified YANG file
</data>
</rpc-reply>
Use the <get-sessions> operation to retrieve NETCONF session information of the device.
# Copy the following message to the client to retrieve NETCONF session information from the device:
<get-sessions/>
</rpc>
If the <get-sessions> operation succeeds, the device returns a response in the following format:
<get-sessions>
<Session>
<SessionID>Configuration session ID</SessionID>
<Line>Line information</Line>
<UserName>Name of the user creating the session</UserName>
<Since>Time when the session was created</Since>
<LockHeld>Whether the session holds a lock</LockHeld>
</Session>
</get-sessions>
</rpc-reply>
Retrieve a data entry for the interface table.
# Enter XML view.
<Sysname> xml
# Notify the device of the NETCONF capabilities supported on the client.
<capabilities>
<capability>urn:ietf:params:netconf:base:1.0</capability>
</capabilities>
</hello>
# Retrieve a data entry for the interface table.
<rpc message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" xmlns:web="urn:ietf:params:xml:ns:netconf:base:1.0">
<get-bulk>
<top xmlns="http://www.h3c.com/netconf/data:1.0" xmlns:web="http://www.h3c.com/netconf/base:1.0">
<Ifmgr>
<Interfaces web:count="1">
</Interfaces>
</Ifmgr>
</top>
</filter>
</get-bulk>
</rpc>
If the client receives the following text, the <get-bulk> operation is successful:
<rpc-reply xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" xmlns:web="urn:ietf:params:xml:ns:netconf:base:1.0" message-id="100">
<data>
<Ifmgr>
<Interfaces>
<Interface>
<IfIndex>3</IfIndex>
<Name>Ten-GigabitEthernet1/0/2</Name>
<AbbreviatedName>XGE1/0/2</AbbreviatedName>
<PortIndex>3</PortIndex>
<ifTypeExt>22</ifTypeExt>
<ifType>6</ifType>
<Description>Ten-GigabitEthernet1/0/2 Interface</Description>
<AdminStatus>2</AdminStatus>
<OperStatus>2</OperStatus>
<ConfigSpeed>0</ConfigSpeed>
<ActualSpeed>100000</ActualSpeed>
<ConfigDuplex>3</ConfigDuplex>
<ActualDuplex>1</ActualDuplex>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</data>
</rpc-reply>
Retrieve all non-default configuration data.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Retrieve all non-default configuration data.
<get-config>
<source>
<running/>
</source>
</get-config>
</rpc>
If the client receives the following text, the <get-config> operation is successful:
<data>
<Ifmgr>
<Interfaces>
<Interface>
<IfIndex>1307</IfIndex>
<Shutdown>1</Shutdown>
</Interface>
<Interface>
<IfIndex>1308</IfIndex>
</Interface>
<Interface>
<IfIndex>1309</IfIndex>
</Interface>
<Interface>
<IfIndex>1311</IfIndex>
<VlanType>2</VlanType>
</Interface>
<Interface>
<IfIndex>1313</IfIndex>
</Interface>
</Interfaces>
</Ifmgr>
<Syslog>
<LogBuffer>
<BufferSize>120</BufferSize>
</LogBuffer>
</Syslog>
<System>
<Device>
<SysName>Sysname</SysName>
<TimeZone>
<Zone>+11:44</Zone>
<ZoneName>beijing</ZoneName>
</TimeZone>
</Device>
</System>
</top>
</data>
</rpc-reply>
Retrieve configuration data for the Syslog module.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Retrieve configuration data for the Syslog module.
<get-config>
<source>
<running/>
</source>
<Syslog/>
</top>
</filter>
</get-config>
</rpc>
<rpc-reply xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" message-id="100">
<data>
<Syslog>
<LogBuffer>
</LogBuffer>
</Syslog>
</top>
</data>
</rpc-reply>
Get NETCONF session information.
# Enter XML view.
<Sysname> xml
# Copy the following message to the client to exchange capabilities with the device:
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Copy the following message to the client to get the current NETCONF session information on the device:
<get-sessions/>
</rpc>
If the client receives a message as follows, the operation is successful:
<get-sessions>
<Session>
<SessionID>1</SessionID>
<Line>vty0</Line>
<UserName></UserName>
<Since>2019-01-07T00:24:57</Since>
<LockHeld>false</LockHeld>
</Session>
</get-sessions>
</rpc-reply>
· The session ID of an existing NETCONF session is 1.
· The login user type is vty0.
· The login time is 2019-01-07T00:24:57.
· The user does not hold the lock of the configuration.
Filtering data
About data filtering
You can define a filter to filter information when you perform a <get>, <get-bulk>, <get-config>, or <get-bulk-config> operation. Data filtering includes the following types:
· Table-based filtering—Filters table information.
· Column-based filtering—Filters information for a single column.
For table-based filtering to take effect, you must configure table-based filtering before column-based filtering.
The namespace is http://www.h3c.com/netconf/base:1.0. The attribute name is filter. For information about the support for table-based match, see the NETCONF XML API references.
# Copy the following text to the client to retrieve the longest data with IP address 1.1.1.0 and mask length 24 from the IPv4 routing table:
<rpc message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" xmlns:h3c="http://www.h3c.com/netconf/base:1.0">
<get>
<Route>
<Ipv4Routes>
<RouteEntry h3c:filter="IP 1.1.1.0 MaskLen 24 longer"/>
</Ipv4Routes>
</Route>
</top>
</filter>
</get>
</rpc>
To use table-based filtering, specify a match criterion for the filter row attribute.
Column-based filtering includes full match filtering, regular expression match filtering, and conditional match filtering. Full match filtering has the highest priority and conditional match filtering has the lowest priority. When more than one filtering criterion is specified, the one with the highest priority takes effect.
You can specify an element value in an XML message to implement full match filtering. If multiple element values are provided, the system returns the data that matches all the specified values.
# Copy the following text to the client to retrieve configuration data of all interfaces in UP state:
<get>
<Ifmgr>
<Interfaces>
<Interface>
<AdminStatus>1</AdminStatus>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get>
</rpc>
You can also specify an attribute name that is the same as a column name of the current table at the row to implement full match filtering. The system returns only configuration data that matches this attribute name. The XML message equivalent to the above element-value-based full match filtering is as follows:
<get>
<top xmlns="http://www.h3c.com/netconf/data:1.0"xmlns:data="http://www.h3c.com/netconf/data:1.0">
<Ifmgr>
<Interfaces>
<Interface data:AdminStatus="1"/>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get>
</rpc>
The above examples show that both element-value-based full match filtering and attribute-name-based full match filtering can retrieve the same index and column information for all interfaces in up state.
Regular expression match filtering
To implement a complex data filtering with characters, you can add a regExp attribute for a specific element.
The supported data types include integer, date and time, character string, IPv4 address, IPv4 mask, IPv6 address, MAC address, OID, and time zone.
# Copy the following text to the client to retrieve the descriptions of interfaces, of which all the characters must be upper-case letters from A to Z:
<get-config>
<source>
<running/>
</source>
<Ifmgr>
<Interfaces>
<Interface>
<Description h3c:regExp="^[A-Z]*$"/>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get-config>
</rpc>
Conditional match filtering
To implement a complex data filtering with digits and character strings, you can add a match attribute for a specific element. Table 3 lists the conditional match operators.
Table 3 Conditional match operators
Operation |
Operator |
Remarks |
More than |
match="more:value" |
More than the specified value. The supported data types include date, digit, and character string. |
Less than |
match="less:value" |
Less than the specified value. The supported data types include date, digit, and character string. |
Not less than |
match="notLess:value" |
Not less than the specified value. The supported data types include date, digit, and character string. |
Not more than |
match="notMore:value" |
Not more than the specified value. The supported data types include date, digit, and character string. |
Equal |
match="equal:value" |
Equal to the specified value. The supported data types include date, digit, character string, OID, and BOOL. |
Not equal |
match="notEqual:value" |
Not equal to the specified value. The supported data types include date, digit, character string, OID, and BOOL. |
Include |
match="include:string" |
Includes the specified string. The supported data types include only character string. |
Not include |
match="exclude:string" |
Excludes the specified string. The supported data types include only character string. |
Start with |
match="startWith:string" |
Starts with the specified string. The supported data types include character string and OID. |
End with |
match="endWith:string" |
Ends with the specified string. The supported data types include only character string. |
# Copy the following text to the client to retrieve extension information about the entity whose CPU usage is more than 50%:
<get>
<Device>
<ExtPhysicalEntities>
<Entity>
<CpuUsage h3c:match="more:50"></CpuUsage>
</Entity>
</ExtPhysicalEntities>
</Device>
</top>
</filter>
</get>
</rpc>
Retrieve all data including Gig in the Description column of the Interfaces table under the Ifmgr module.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Retrieve all data including Gig in the Description column of the Interfaces table under the Ifmgr module.
<get>
<Ifmgr>
<Interfaces>
<Interface>
<Description h3c:regExp="(Gig)+"/>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get>
</rpc>
If the client receives the following text, the operation is successful:
<rpc-reply xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" xmlns:h3c="http://www.h3c.com/netconf/base:1.0" message-id="100">
<data>
<Ifmgr>
<Interfaces>
<Interface>
<IfIndex>2681</IfIndex>
<Description>Ten-GigabitEthernet1/0/1 Interface</Description>
</Interface>
<Interface>
<IfIndex>2685</IfIndex>
</Interface>
<Interface>
<IfIndex>2689</IfIndex>
<Description>Ten-GigabitEthernet1/0/3 Interface</Description>
</Interface>
<Interface>
</Ifmgr>
</top>
</data>
</rpc-reply>
Retrieve data in the Name column with the ifindex value not less than 5000 in the Interfaces table under the Ifmgr module.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Retrieve data in the Name column with the ifindex value not less than 5000 in the Interfaces table under the Ifmgr module.
<get>
<Ifmgr>
<Interfaces>
<Interface>
<IfIndex h3c:match="notLess:5000"/>
<Name/>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get>
</rpc>
<data>
<Ifmgr>
<Interfaces>
<Interface>
<IfIndex>7241</IfIndex>
<Name>NULL0</Name>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</data>
</rpc-reply>
Multiple methods are available for configuring the device, such as CLI, NETCONF, and SNMP. Before configuring, managing, or troubleshooting the device, you can lock the configuration to prevent other users from changing the device configuration. After you lock the configuration, only you can perform <edit-config> operations to change the configuration or unlock the configuration. Other users can only read the configuration.
If you close your NETCONF session, the system unlocks the configuration. You can also manually unlock the configuration.
The <lock> operation locks the running configuration of the device. You cannot use it to lock the configuration for a specific module.
# Copy the following text to the client to lock the running configuration:
<lock>
<target>
<running/>
</target>
</lock>
</rpc>
If the <lock> operation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
# Copy the following text to the client to unlock the running configuration:
<unlock>
<target>
<running/>
</target>
</unlock>
</rpc>
If the <unlock> operation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
Lock the device configuration so other users cannot change the device configuration.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Lock the configuration.
<lock>
<target>
<running/>
</target>
</lock>
</rpc>
If the client receives the following response, the <lock> operation is successful:
<ok/>
</rpc-reply>
If another client sends a lock request, the device returns the following response:
<rpc-error>
<error-type>protocol</error-type>
<error-tag>lock-denied</error-tag>
<error-severity>error</error-severity>
<error-message xml:lang="en"> Lock failed because the NETCONF lock is held by another session.</error-message>
<error-info>
</error-info>
</rpc-error>
</rpc-reply>
The output shows that the <lock> operation failed. The client with session ID 1 is holding the lock,
The <edit-config> operation includes the following operations: merge, create, replace, remove, delete, default-operation, error-option, test-option, and incremental. For more information about the operations, see "Supported NETCONF operations."
# Copy the following text to perform the <edit-config> operation:
<edit-config>
<target><running></running></target>
<error-option>
error-option
</error-option>
<config>
</top>
</config>
</edit-config>
</rpc>
The <error-option> element indicates the action to be taken in response to an error that occurs during the operation. It has the following values:
Value |
stop-on-error |
Stops the <edit-config> operation. |
continue-on-error |
Continues the <edit-config> operation. |
rollback-on-error |
Rolls back the configuration to the configuration before the <edit-config> operation was performed. By default, an <edit-config> operation cannot be performed while the device is rolling back the configuration. If the rollback time exceeds the maximum time that the client can wait, the client determines that the <edit-config> operation has failed and performs the operation again. Because the previous rollback is not completed, the operation triggers another rollback. If this process repeats itself, CPU and memory resources will be exhausted and the device will reboot. To allow an <edit-config> operation to be performed during a configuration rollback, perform an <action> operation to change the value of the DisableEditConfigWhenRollback attribute to false. |
If the <edit-config> operation succeeds, the device returns a response in the following format:
<?xml version="1.0">
<ok/>
</rpc-reply>
You can also perform the <get> operation to verify that the current element value is the same as the value specified through the <edit-config> operation.
Change the log buffer size for the Syslog module to 512.
# Enter XML view.
<Sysname> xml
<capabilities>
</capabilities>
</hello>
# Change the log buffer size for the Syslog module to 512.
<edit-config>
<target>
<running/>
</target>
<config>
<top xmlns="http://www.h3c.com/netconf/config:1.0" web:operation="merge">
<Syslog>
<LogBuffer>
<BufferSize>512</BufferSize>
</LogBuffer>
</Syslog>
</top>
</config>
</edit-config>
</rpc>
If the client receives the following text, the <edit-config> operation is successful:
<ok/>
</rpc-reply>
About the <save> operation
A <save> operation saves the running configuration to a configuration file and specifies the file as the main next-startup configuration file.
The <save> operation is resource intensive. Do not perform this operation when system resources are heavily occupied.
# Copy the following text to the client:
<save OverWrite="false" Safely="false">
<file>Configuration file name</file>
</save>
</rpc>
Item |
file |
Specifies a .cfg configuration file by its name. The name must start with the storage medium name. If you specify the file column, a file name is required. If the Binary-only attribute is false, the device saves the running configuration to both the text and binary configuration files. · If the specified .cfg file does not exist, the device creates the binary and text configuration files to save the running configuration. · If you do not specify the file column, the device saves the running configuration to the text and binary next-startup configuration files. |
OverWrite |
Determines whether to overwrite the specified file if the file already exists. The following values are available: · true—Overwrite the file. · false—Do not overwrite the file. The running configuration cannot be saved, and the system displays an error message. The default value is true. |
Safely |
Determines whether to save the configuration file in safe mode or fast mode. Available values: · true—Saves the configuration in safe mode. In this mode, the system saves the configuration in a temporary file and starts overwriting the target next-startup configuration file after the save operation is complete. If a disruptive event such as a reboot or power failure occurs during the save operation, the device can still start up with the original next-startup configuration file. · false—Saves the configuration in fast mode. In this mode, the system directly overwrites the target next-startup configuration file. If a disruptive event such as a reboot, power failure, out-of-memory, out-of-storage event occurs during this process, the next-startup configuration file is lost. You must specify a new startup configuration file after the device reboots. By default, the Safely attribute is set to false if you do not specify a value for it. Safe mode is slower than fast mode, but more secure. As a best practice, use the safe mode if the power source is not reliable or you are remotely configuring the device. |
If the <save> operation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
Save the running configuration to the config.cfg file.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Save the running configuration of the device to the config.cfg file.
<save>
<file>config.cfg</file>
</save>
</rpc>
If the client receives the following response, the <save> operation is successful:
<ok/>
</rpc-reply>
Loading the configuration
About the <load> operation
The <load> operation merges the configuration from a configuration file into the running configuration as follows:
· Loads settings that do not exist in the running configuration.
· Overwrites settings that already exist in the running configuration.
When you perform a <load> operation, follow these restrictions and guidelines:
· The <load> operation is resource intensive. Do not perform this operation when the system resources are heavily occupied.
· Some settings in a configuration file might conflict with the existing settings. For the settings in the file to take effect, delete the existing conflicting settings, and then load the configuration file.
# Copy the following text to the client to load a configuration file for the device:
<load>
</load>
</rpc>
The configuration file name must start with the storage media name and end with the .cfg extension.
If the <load> operation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
The <rollback> operation is resource intensive. Do not perform this operation when the system resources are heavily occupied.
By default, an <edit-config> operation cannot be performed while the device is rolling back the configuration. To allow an <edit-config> operation to be performed during a configuration rollback, perform an <action> operation to change the value of the DisableEditConfigWhenRollback attribute to false.
# Copy the following text to the client to roll back the running configuration to the configuration in a configuration file:
<rollback>
<file>Specify the configuration file name</file>
</rollback>
</rpc>
If the <rollback> operation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
You can roll back the running configuration based on a rollback point when one of the following situations occurs:
· A NETCONF client sends a rollback request.
· The NETCONF session idle time is longer than the rollback idle timeout time.
· A NETCONF client is unexpectedly disconnected from the device.
Multiple users might simultaneously configure the device. As a best practice, lock the system before rolling back the configuration to prevent other users from modifying the running configuration.
1. Lock the running configuration. For more information, see "Locking or unlocking the running configuration."
2. Enable configuration rollback based on a rollback point.
# Copy the following text to the client to perform a <save-point>/<begin> operation:
<save-point>
<begin>
<confirm-timeout>100</confirm-timeout>
</begin>
</save-point>
</rpc>
Item |
confirm-timeout |
Specifies the rollback idle timeout time in the range of 1 to 65535 seconds. The default is 600 seconds. This item is optional. |
If the <save-point/begin> operation succeeds, the device returns a response in the following format:
<data>
<save-point>
<commit>
<commit-id>1</commit-id>
</commit>
</save-point>
</data>
</rpc-reply>
3. Modify the running configuration. For more information, see "Modifying the configuration."
4. Mark the rollback point.
The system supports a maximum of 50 rollback points. If the limit is reached, specify the force attribute for the <save-point>/<commit> operation to overwrite the earliest rollback point.
# Copy the following text to the client to perform a <save-point>/<commit> operation:
<save-point>
<commit>
<label>SUPPORT VLAN<label>
<comment>vlan 1 to 100 and interfaces.</comment>
</commit>
</save-point>
</rpc>
The <label> and <comment> elements are optional.
If the <save-point>/<commit> operation succeeds, the device returns a response in the following format:
<data>
<save-point>
<commit>
<commit-id>2</commit-id>
</commit>
</save-point>
</data>
</rpc-reply>
5. Retrieve the rollback point configuration records.
The following text shows the message format for a <save-point/get-commits> request:
<save-point>
<get-commits>
<commit-id/>
<commit-index/>
<commit-label/>
</get-commits>
</save-point>
</rpc>
Specify the <commit-id/>, <commit-index/>, or <commit-label/> element to retrieve the specified rollback point configuration records. If no element is specified, the operation retrieves records for all rollback point settings.
# Copy the following text to the client to perform a <save-point>/<get-commits> operation:
<save-point>
<get-commits>
<commit-label>SUPPORT VLAN</commit-label>
</get-commits>
</save-point>
</rpc>
If the <save-point/get-commits> operation succeeds, the device returns a response in the following format:
<data>
<save-point>
<commit-information>
<CommitID>2</CommitID>
<TimeStamp>Sun Jan 1 11:30:28 2019</TimeStamp>
<UserName>test</UserName>
<Label>SUPPORT VLAN</Label>
</commit-information>
</save-point>
</data>
</rpc-reply>
6. Retrieve the configuration data corresponding to a rollback point.
The following text shows the message format for a <save-point>/<get-commit-information> request:
<save-point>
<commit-id/>
<commit-index/>
<commit-label/>
<compare-information>
<commit-id/>
<commit-index/>
<commit-label/>
</compare-information>
</get-commit-information>
</save-point>
</rpc>
Specify one of the following elements: <commit-id/>, <commit-index/>, and <commit-label/>. The <compare-information> element is optional.
Item |
commit-id |
Uniquely identifies a rollback point. |
commit-index |
Specifies 50 most recently configured rollback points. The value of 0 indicates the most recently configured one and 49 indicates the earliest configured one. |
commit-label |
Specifies a unique label for a rollback point. |
get-commit-information |
Retrieves the configuration data corresponding to the most recently configured rollback point. |
# Copy the following text to the client to perform a <save-point>/<get-commit-information> operation:
<save-point>
</save-point>
</rpc>
If the <save-point/get-commit-information> operation succeeds, the device returns a response in the following format:
<data>
<save-point>
<content>
interface vlan 1
</content>
</save-point>
</data>
</rpc-reply>
7. Roll back the configuration based on a rollback point.
The configuration can also be automatically rolled back based on the most recently configured rollback point when the NETCONF session idle timer expires.
# Copy the following text to the client to perform a <save-point>/<rollback> operation:
<save-point>
<rollback>
<commit-id/>
<commit-index/>
<commit-label/>
</rollback>
</save-point>
</rpc>
Specify one of the following elements: <commit-id/>, <commit-index/>, and <commit-label/>. If no element is specified, the operation rolls back configuration based on the most recently configured rollback point.
Item |
commit-id |
commit-index |
commit-label |
Specifies the unique label of a rollback point. |
If the <save-point/rollback> operation succeeds, the device returns a response in the following format:
<ok></ok>
</rpc-reply>
8. End the rollback configuration.
# Copy the following text to the client to perform a <save-point>/<end> operation:
<save-point>
<end/>
</save-point>
</rpc>
If the <save-point/end> operation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
9. Unlock the configuration. For more information, see "Locking or unlocking the running configuration."
You can enclose command lines in XML messages to configure the device.
Performing CLI operations through NETCONF is resource intensive. As a best practice, do not perform the following tasks:
· Enclose multiple command lines in one XML message.
· Use NETCONF to perform a CLI operation when other users are performing NETCONF CLI operations.
# Copy the following text to the client to execute the commands:
<CLI>
<Execution>
Commands
</Execution>
</CLI>
</rpc>
The <Execution> element can contain multiple commands, with one command on one line.
If the CLI operation succeeds, the device returns a response in the following format:
<CLI>
<Execution>
<![CDATA[Responses to the commands]]>
</Execution>
</CLI>
</rpc-reply>
Send the display vlan command to the device.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Copy the following text to the client to execute the display vlan command:
<CLI>
<Execution>
display vlan
</Execution>
</CLI>
</rpc>
<CLI>
<Execution><![CDATA[
<Sysname>display vlan
Total VLANs: Problem 12 1
The VLANs include:
1(default)
</Execution>
</CLI>
</rpc-reply>
About event subscription
When an event takes place on the device, the device sends information about the event to NETCONF clients that have subscribed to the event.
Event subscription is not supported for NETCONF over SOAP sessions.
A subscription takes effect only on the current session. It is canceled when the session is terminated.
If you do not specify the event stream to be subscribed to, the device sends syslog event notifications to the NETCONF client.
# Copy the following message to the client to complete the subscription:
<create-subscription xmlns="urn:ietf:params:xml:ns:netconf:notification:1.0">
<stream>NETCONF</stream>
<filter>
<event xmlns="http://www.h3c.com/netconf/event:1.0">
<Code>code</Code>
<Group>group</Group>
<Severity>severity</Severity>
</event>
</filter>
<startTime>start-time</startTime>
<stopTime>stop-time</stopTime>
</create-subscription>
</rpc>
Item |
stream |
Specifies the event stream. The name for the syslog event stream is NETCONF. |
event |
Specifies the event. For information about the events to which you can subscribe, see the system log message references for the device. |
code |
Specifies the mnemonic symbol of the log message. |
group |
Specifies the module name of the log message. |
severity |
Specifies the severity level of the log message. |
start-time |
Specifies the start time of the subscription. |
stop-time |
Specifies the end time of the subscription. |
If the subscription succeeds, the device returns a response in the following format:
<rpc-reply message-id="100" xmlns:netconf="urn:ietf:params:xml:ns:netconf:base:1.0">
<ok/>
</rpc-reply>
If the subscription fails, the device returns an error message in the following format:
<rpc-error>
<error-type>error-type</error-type>
<error-tag>error-tag</error-tag>
<error-severity>error-severity</error-severity>
<error-message xml:lang="en">error-message</error-message>
</rpc-error>
</rpc-reply>
For more information about error messages, see RFC 4741.
After you subscribe to events as described in this section, NETCONF regularly polls the subscribed events and sends the events that match the subscription condition to the NETCONF client.
<create-subscription xmlns='urn:ietf:params:xml:ns:netconf:notification:1.0'>
<stream>NETCONF_MONITOR_EXTENSION</stream>
<filter>
<NetconfMonitor xmlns='http://www.h3c.com/netconf/monitor:1.0'>
<XPath>XPath</XPath>
<Interval>interval</Interval>
<ColumnConditions>
<ColumnCondition>
<ColumnName>ColumnName</ColumnName>
<ColumnValue>ColumnValue</ColumnValue>
<ColumnCondition>ColumnCondition</ColumnCondition>
</ColumnCondition>
</ColumnConditions>
<MustIncludeResultColumns>
<ColumnName>columnName</ColumnName>
</MustIncludeResultColumns>
</filter>
</rpc>
Item |
stream |
Specifies the event stream. The name for the event stream is NETCONF_MONITOR_EXTENSION. |
NetconfMonitor |
Specifies the filtering information for the event. |
XPath |
Specifies the path of the event in the format of ModuleName[/SubmoduleName]/TableName. |
interval |
Specifies the interval for NETCONF to obtain events that matches the subscription condition. The value range is 1 to 4294967 seconds. The default value is 300 seconds. |
ColumnName |
Specifies the name of a column in the format of [GroupName.]ColumnName. |
ColumnValue |
Specifies the baseline value. |
ColumnCondition |
Specifies the operator: · more. · less. · notLess. · notMore. · equal. · notEqual. · include. · exclude. · startWith. · endWith. Choose an operator according to the type of the baseline value. |
start-time |
stop-time |
<ok/>
</rpc-reply>
After you subscribe to events as described in this section, the specified modules report subscribed events to NETCONF. NETCONF sends the events to the NETCONF client.
<rpc message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" xmlns:xs="http://www.h3c.com/netconf/base:1.0">
<stream>XXX_STREAM</stream>
<event xmlns="http://www.h3c.com/netconf/event:1.0/xxx-features-list-name:1.0">
<ColumnName xs:condition="Condition">value</ColumnName>
</event>
</filter>
</rpc>
Item |
stream |
Specifies the event stream. Supported event streams vary by device model. |
event |
Specifies the event name. An event stream includes multiple events. The events use the same namespaces as the event stream. |
ColumnName |
Specifies the name of a column. |
Condition |
value |
Specifies the baseline value for the column. |
start-time |
stop-time |
<ok/>
</rpc-reply>
# Copy the following message to the client to cancel a subscription:
<cancel-subscription xmlns="urn:ietf:params:xml:ns:netconf:notification:1.0">
</cancel-subscription>
</rpc>
Item |
stream |
Specifies the event stream. |
If the cancelation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
If the subscription to be canceled does not exist, the device returns an error message in the following format:
<rpc-error>
<error-message xml:lang="en">The subscription stream to be canceled doesn't exist: Stream name=XXX_STREAM.</error-message>
</rpc-error>
</rpc-reply>
Configure a client to subscribe to syslog events with no time limitation. After the subscription, all events on the device are sent to the client before the session between the device and client is terminated.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Subscribe to syslog events with no time limitation.
</rpc>
# If the client receives the following response, the subscription is successful:
<ok/>
</rpc-reply>
# When another client (192.168.100.130) logs in to the device, the device sends a notification to the client that has subscribed to all events:
<notification xmlns="urn:ietf:params:xml:ns:netconf:notification:1.0">
<eventTime>2019-01-04T12:30:52</eventTime>
<Group>SHELL</Group>
<Code>SHELL_LOGIN</Code>
<Slot>1</Slot>
<Severity>Notification</Severity>
<context>VTY logged in from 192.168.100.130.</context>
</event>
</notification>
NETCONF allows one client to terminate the NETCONF sessions of other clients. A client whose session is terminated returns to user view.
# Copy the following message to the client to terminate a NETCONF session:
<kill-session>
<session-id>
Specified session-ID
</session-id>
</kill-session>
</rpc>
If the <kill-session> operation succeeds, the device returns a response in the following format:
<ok/>
</rpc-reply>
The user whose session's ID is 1 terminates the session with session ID 2.
# Enter XML view.
<Sysname> xml
<capabilities>
<capability>
</capability>
</capabilities>
</hello>
# Terminate the session with session ID 2.
<rpc message-id="100"xmlns="urn:ietf:params:xml:ns:netconf:base:1.0">
<kill-session>
<session-id>2</session-id>
</kill-session>
</rpc>
If the client receives the following text, the NETCONF session with session ID 2 has been terminated, and the client with session ID 2 has returned from XML view to user view:
<ok/>
</rpc-reply>
Before returning from XML view to the CLI, you must first complete capability exchange between the device and the client.
# Copy the following text to the client to return from XML view to the CLI:
<close-session/>
</rpc>
When the device receives the close-session request, it sends the following response and returns to CLI's user view:
<ok/>
</rpc-reply>
To report critical NETCONF events to an SNMP NMS, enable SNMP notifications for NETCONF. For NETCONF SNMP notifications to be sent correctly, you must also configure SNMP on the device. For more information about configuring SNMP, see Network Management and Monitoring Configuration Guide.
2. Enable SNMP notifications for NETCONF.
snmp-agent trap enable netconf
By default, SNMP notifications are enabled for NETCONF.
Task |
Command |
Display current NETCONF service status and global NETCONF service statistics. |
display netconf service |
Display NETCONF session status and statistics. |
display netconf session |
Clear NETCONF service statistics. |
reset netconf service statistics |
Clear NETCONF session statistics. |
reset netconf session statistics |
This chapter describes NETCONF operations available with Comware 7.
action
This operation sends a non-configuration operation instruction to the device, for example, a reset instruction.
XML example
# Clear statistics information for all interfaces.
<action>
<top xmlns="http://www.h3c.com/netconf/action:1.0">
<Ifmgr>
<ClearAllIfStatistics>
<Clear>
</Clear>
</ClearAllIfStatistics>
</Ifmgr>
</top>
</action>
</rpc>
CLI
This operation executes CLI commands.
A request message encloses commands in the <CLI> element. A response message encloses the command output in the <CLI> element.
You can use the following elements to execute commands:
· Execution—Executes commands in user view.
· Configuration—Executes commands in system view.
To use this element, include the exec-use-channel attribute and specify a value for the attribute:
¡ false—Executes commands without using a channel.
¡ true—Executes commands by using a temporary channel. The channel is automatically closed after the execution.
¡ persist—Executes commands by using the persistent channel for the session.
To use the persistent channel, first perform an <Open-channel> operation to open the persistent channel. If you do not do so, the system will automatically open the persistent channel.
After using the persistent channel, perform a <Close-channel> operation to close the channel and return to system view. If you do not perform an <Open-channel> operation, the system stays in the view and will execute subsequent commands in the view.
You can also specify the error-when-rollback attribute in the <Configuration> element to indicate whether CLI operations are allowed during a configuration error-triggered configuration rollback. This attribute takes effect only if the value of the <error-option> element in <edit-config> operations is set to rollback-on-error. It has the following values:
¡ true—Rejects CLI operation requests and returns error messages.
¡ false (the default)—Allows CLI operations.
For CLI operations to be correctly performed, set the value of the error-when-rollback attribute to true.
NOTE: To execute commands in a lower-level view of the system view, use the <Configuration> element to enter the view first. |
A NETCONF session can have multiple temporary channels, but it can have only one persistent channel.
This operation does not support executing interactive CLI commands.
You cannot execute the quit command by using a channel to exit user view.
XML example
# Execute the vlan 3 command in system view without using a channel.
<CLI>
<Configuration exec-use-channel="false" error-when-rollback="true">vlan 3</Configuration>
</CLI>
</rpc>
close-session
This operation terminates the current NETCONF session, unlocks the configuration, and releases the resources (for example, memory) used by the session. After this operation, you exit the XML view.
XML example
# Terminate the current NETCONF session.
<close-session/>
</rpc>
edit-config: create
This operation creates target configuration items.
To use the create attribute in an <edit-config> operation, you must specify the target configuration item.
· If the table supports creating a target configuration item and the item does not exist, the operation creates the item and configures the item.
· If the specified item already exists, a data-exist error message is returned.
XML example
# Set the buffer size to 120.
<rpc message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0" xmlns:xc="urn:ietf:params:xml:ns:netconf:base:1.0">
<edit-config>
<target>
<running/>
</target>
<config>
<Syslog xmlns="http://www.h3c.com/netconf/config:1.0" xc:operation="create">
<LogBuffer>
</LogBuffer>
</Syslog>
</top>
</config>
</edit-config>
</rpc>
edit-config: delete
This operation deletes the specified configuration.
· If the specified target has only the table index, the operation removes all configuration of the specified target, and the target itself.
· If the specified target has the table index and configuration data, the operation removes the specified configuration data of this target.
· If the specified target does not exist, an error message is returned, showing that the target does not exist.
XML example
The syntax is the same as the edit-config message with the create attribute. Change the operation attribute from create to delete.
edit-config: merge
This operation commits target configuration items to the running configuration.
To use the merge attribute in an <edit-config> operation, you must specify the target configuration item (on a specific level):
· If the specified item exists, the operation directly updates the setting for the item.
· If the specified item does not exist, the operation creates the item and configures the item.
· If the specified item does not exist and it cannot be created, an error message is returned.
XML example
edit-config: remove
This operation removes the specified configuration.
· If the specified target does not exist, or the XML message does not specify any targets, a success message is returned.
XML example
The syntax is the same as the edit-config message with the create attribute. Change the operation attribute from create to remove.
edit-config: replace
This operation replaces the specified configuration.
· If the specified target exists, the operation replaces the configuration of the target with the configuration carried in the message.
· If the specified target does not exist but is allowed to be created, the operation creates the target and then applies the configuration.
· If the specified target does not exist and is not allowed to be created, the operation is not conducted and an invalid-value error message is returned.
XML example
The syntax is the same as the edit-config message with the create attribute. Change the operation attribute from create to replace.
edit-config: test-option
This operation determines whether to commit a configuration item in an <edit-configure> operation. The <test-option> element has one of the following values:
· test-then-set—Performs a syntax check, and commits an item if the item passes the check. If the item fails the check, the item is not committed. This is the default test-option value.
· set—Commits the item without performing a syntax check.
· test-only—Performs only a syntax check. If the item passes the check, a success message is returned. Otherwise, an error message is returned.
XML example
# Test the configuration for an interface.
<rpc message-id="100" xmlns="urn:ietf:params:xml:ns:netconf:base:1.0">
<edit-config>
<target>
<running/>
</target>
<test-option>test-only</test-option>
<config xmlns:xc="urn:ietf:params:xml:ns:netconf:base:1.0">
<Ifmgr xc:operation="merge">
<Interfaces>
<Interface>
<IfIndex>262</IfIndex>
<Description>222</Description>
<ConfigSpeed>2</ConfigSpeed>
<ConfigDuplex>1</ConfigDuplex>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</config>
</edit-config>
</rpc>
edit-config: default-operation
This operation modifies the running configuration of the device by using the default operation method.
NETCONF uses one of the following operation attributes to modify configuration: merge, create, delete, and replace. If you do not specify an operation attribute for an edit-config message, NETCONF uses the default operation method. The value specified for the <default-operation> element takes effect only once. If you do not specify an operation attribute or the default operation method for an <edit-config> message, merge always applies.
The <default-operation> element has the following values:
· merge—Default value for the <default-operation> element.
· replace—Value used when the operation attribute is not specified and the default operation method is specified as replace.
· none—Value used when the operation attribute is not specified and the default operation method is specified as none. If this value is specified, the <edit-config> operation is used only for schema verification rather than issuing a configuration. If the schema verification is passed, a successful message is returned. Otherwise, an error message is returned.
XML example
# Issue an empty operation for schema verification purposes.
<edit-config>
<target>
<running/>
</target>
<default-operation>none</default-operation>
<Ifmgr>
<Interfaces>
<Interface>
<Description>222222</Description>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</config>
</edit-config>
</rpc>
edit-config: error-option
This operation determines the action to take in case of a configuration error.
The <error-option> element has the following values:
· stop-on-error—Stops the operation and returns an error message. This is the default error-option value.
· continue-on-error—Continues the operation and returns an error message.
· rollback-on-error—Rolls back the configuration.
XML example
# Issue the configuration for two interfaces, setting the <error-option> element to continue-on-error.
<edit-config>
<target>
<running/>
</target> <error-option>continue-on-error</error-option>
<Interfaces>
<Interface>
<ConfigSpeed>1024</ConfigSpeed>
</Interface>
<Interface>
<IfIndex>263</IfIndex>
<Description>333</Description>
</Interface>
</Interfaces>
</Ifmgr>
</top>
</config>
</edit-config>
</rpc>
edit-config: incremental
This operation adds configuration data to a column without affecting the original data.
The incremental attribute applies to a list column such as the vlan permitlist column.
You can use the incremental attribute for <edit-config> operations with an attribute other than replace.
Support for the incremental attribute varies by module. For more information, see NETCONF XML API references.
XML example
# Add VLANs 1 through 10 to an untagged VLAN list that has untagged VLANs 12 through 15.
<edit-config>
<target>
<running/>
</target>
<VLAN xc:operation="merge">
<HybridInterfaces>
<Interface>
<UntaggedVlanList h3c:incremental="true">1-10</UntaggedVlanList>
</Interface>
</HybridInterfaces>
</VLAN>
</top>
</config>
</edit-config>
</rpc>
get
This operation retrieves device configuration and state information.
XML example
# Retrieve device configuration and state information for the Syslog module.
<get>
<filter type="subtree">
<top xmlns="http://www.h3c.com/netconf/data:1.0">
<Syslog>
</Syslog>
</top>
</filter>
</get>
</rpc>
get-bulk
This operation retrieves a number of data entries (including device configuration and state information) starting from the data entry next to the one with the specified index.
XML example
# Retrieve device configuration and state information for all interfaces.
<get-bulk>
<Ifmgr>
<Interfaces xc:count="5" xmlns:xc="http://www.h3c.com/netconf/base:1.0">
<Interface/>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get-bulk>
</rpc>
get-bulk-config
This operation retrieves a number of non-default configuration data entries starting from the data entry next to the one with the specified index.
XML example
# Retrieve non-default configuration for all interfaces.
<get-bulk-config>
<source>
<running/>
</source>
<Ifmgr>
</Ifmgr>
</top>
</filter>
</get-bulk-config>
</rpc>
get-config
This operation retrieves non-default configuration data. If no non-default configuration data exists, the device returns a response with empty data.
XML example
# Retrieve non-default configuration data for the interface table.
<get-config>
<source>
<running/>
</source>
<Ifmgr>
<Interfaces>
<Interface/>
</Interfaces>
</Ifmgr>
</top>
</filter>
</get-config>
</rpc>
get-sessions
This operation retrieves information about all NETCONF sessions in the system. You cannot specify a session ID to retrieve information about a specific NETCONF session.
XML example
# Retrieve information about all NETCONF sessions in the system.
<get-sessions/>
</rpc>
kill-session
This operation terminates the NETCONF session for another user. This operation cannot terminate the NETCONF session for the current user.
XML example
# Terminate the NETCONF session with session ID 1.
<kill-session>
</kill-session>
</rpc>
load
This operation loads the configuration. After the device finishes a <load> operation, the configuration in the specified file is merged into the running configuration of the device.
XML example
# Merge the configuration in file a1.cfg to the running configuration of the device.
<load>
<file>a1.cfg</file>
</load>
</rpc>
lock
This operation locks the configuration. After you lock the configuration, other users cannot perform <edit-config> operations. Other NETCONF operations are allowed.
After a user locks the configuration, other users cannot use NETCONF or any other configuration methods such as CLI and SNMP to configure the device.
XML example
<lock>
<target>
<running/>
</target>
</lock>
</rpc>
rollback
This operation rolls back the configuration. To do so, you must specify the configuration file in the <file> element. After the device finishes the <rollback> operation, the current device configuration is totally replaced with the configuration in the specified configuration file.
XML example
# Roll back the running configuration to the configuration in file 1A.cfg.
<rollback>
<file>1A.cfg</file>
</rollback>
</rpc>
save
This operation saves the running configuration. You can use the <file> element to specify a file for saving the configuration. If the text does not include the file column, the running configuration is automatically saved to the main next-startup configuration file.
The OverWrite attribute determines whether the running configuration overwrites the original configuration file when the specified file already exists.
The Safely attribute determines whether to save the configuration file in safe mode or fast mode.
XML example
# Save the running configuration to file test.cfg.
<save OverWrite="false">
<file>test.cfg</file>
</save>
</rpc>
unlock
This operation unlocks the configuration, so other users can configure the device.
Terminating a NETCONF session automatically unlocks the configuration.
XML example
# Unlock the configuration.
<unlock>
<target>
<running/>
</target>
</unlock>
</rpc>