| 01-Installation Guide | 2.18 MB |
Examining the installation environment
Examining the installation site
Checking power distribution or power supply environment
Installing the switch in a 19-inch rack
Installation procedure at a glance
Attaching the front mounting brackets to the switch
Mounting the switch in the rack
Mounting the switch on a workbench
Grounding the switch by using a grounding strip
Grounding the switch with a grounding conductor buried in the earth ground
Verifying the connection after grounding the switch
Installing and removing fan trays
Installing and removing power supplies
Installing and removing a power supply (1)
Installing and removing a power supply (2)
Connecting the power cord for a PSR75-12A, CA-70A12, PSR180-12A-F, or PSR180-12A-B power supply
Connecting the power cord for a PSR600-54A-B, PSR920-54A-B, or PSR1600-54A-B power supply
Connecting the power cord for a PSR180-12D-B power supply
Installing and removing expansion cards
3 Accessing the switch for the first time
Connecting the switch to a configuration terminal
Connecting a DB9-to-RJ45 console cable
Connecting a USB-to-RJ45 console cable
4 Maintenance and troubleshooting
No display on the configuration terminal
Garbled display on the configuration terminal
1 Preparing for installation
This document is applicable to the following switches:
Table1-1 Switch series and models
Switch series |
Model |
Product code (PID) |
S5580S-EI switch series |
Non-PoE models |
S5580S-24T6X-EI |
LS-5580S-24T6X-EI |
S5580S-48T6X-EI |
LS-5580S-48T6X-EI |
S5580X-EI switch series |
Non-PoE models |
S5580X-24T6Y-EI |
LS-5580X-24T6Y-EI |
S5580X-48T6Y-EI |
LS-5580X-48T6Y-EI |
S5580X-HI switch series |
PoE models |
S5580X-32P4X4YC-HI |
LS-5580X-32P4X4YC-HI |
S5580X-48P4YC-HI |
LS-5580X-48P4YC-HI |
Non-PoE models |
S5580X-32S8T4X4YC-HI |
LS-5580X-32S8T4X4YC-HI |
S5580X-48S4YC-HI |
LS-5580X-48S4YC-HI |
S5580X-32T4X4YC-HI |
LS-5580X-32T4X4YC-HI |
S5580X-48T4YC-HI |
LS-5580X-48T4YC-HI |
Safety recommendations
To avoid device damage or bodily injury, read the following safety recommendations before installation. Note that the recommendations do not cover every possible hazardous condition.
· Before cleaning the switch, remove all power cords from the switch. Do not clean the switch with wet cloth or liquid.
· Do not place the switch near water or in a damp environment. Prevent water or moisture from entering the switch chassis.
· Do not place the switch on an unstable case or desk. The switch might be severely damaged in case of a fall.
· Ensure good ventilation at the installation site and keep the air inlet and outlet vents of the switch free of obstruction.
· Make sure the power source voltage is as required by the power supply.
· To avoid electrical shocks, do not open the chassis while the switch is operating or when the switch is just powered off.
· During switch installation, wear an ESD wrist strap. Make sure the strap makes good skin contact and is reliably grounded.
To ensure correct operation of your switch, make sure the installation environment meets the requirements listed in Table1-2.
Table1-2 Checking list for the installation environment
Item |
Requirements |
Ventilation and heat dissipation |
To ensure correct operation of your device, make sure the installation environment is adequately ventilated to prevent the switch from overheating. · Ensure a minimum clearance of 10 cm (3.94 in) around the chassis. · Do not install the device near a heat source, for example, a stove or heater. · Ensure air ventilation in the installation environment. · Do not block the ventilation holes in the device or power adapter. |
Anti-moisture |
Water or moisture might damage the circuits of the device. · Do not place the device near water or in a damp environment. · Install the switch in a clean, dry, and ventilated place where temperature is controlled in a stable range. · Make sure the installation environment is free from water leakage or condensation. If required, install a dehumidification device (such as an air conditioner with a dehumidification function or a dedicated dehumidifier). · Do not operate the device under or near the water source, such as the wash basin, laundry room, or areas with high humidity. · Do not touch the device with wet hands. |
Temperature/humidity |
For correct operation and long service life of your switch, maintain the temperature and humidity in the equipment room at acceptable ranges. · Lasting high relative humidity can cause poor insulation, electricity leakage, mechanical property change of materials, and metal corrosion. · Lasting low relative humidity can cause washer contraction and ESD and cause issues including loose mounting screws and circuit failure. · High temperature can accelerate the aging of insulation materials and significantly lower the reliability and lifespan of the switch. For the temperature and humidity requirements of the switch, see technical specifications in S5580S-EI & S5580X-EI Switch Series Hardware Information and Specifications. |
Lightning protection |
Ground the switch correctly and verify the grounding. For more information, see "Grounding the switch." · If you ground the switch by using a grounding strip, make sure the grounding resistance of the grounding strip in the equipment room is less than 1W. · If you ground the switch by using a grounding conductor buried in the earth ground, make sure the grounding resistance of the grounding conductor in the ground is less than 10W. · Route the signal cables along indoor walls, bury the cables in the earth ground, or thread the cables through steel tubes. Install a signal lightning arrester with a nominal discharge current for a corresponding network interface. · Keep the signal cables far from power cords and lightning rod down conductors. · As a best practice, route power cords indoors. If an AC power cord is routed from outdoors, connect the AC power cord first to a power lightning arrester before leading it to the AC power port on the switch. Make sure the power lightning arrester has a nominal discharge current and the total length of the power cord from the power lighting arrester to the power port on the switch is less than 5 m (16.40 ft). · Ground the switch, rack, independent power supplies, and lightning arresters separately. · You must ground optical fibers with reinforcing metal stiffener from outdoors on an optical distribution frame (ODF) or fiber splice enclosure. |
Cable routing |
Do not run an Ethernet cable and power cord in parallel. · Route different types of cables separately. · Keep power cords a minimum of 5 cm (1.97 in) away from other cables. |
ESD prevention |
· Ground the switch correctly. · To avoid ESD damage to the device or components, always wear an ESD wrist strap when you install or remove the device or components. · Make sure the wrist strap has good skin contact and is reliably grounded. |
Cleanliness |
For more information, see "Cleanliness." |
Corrosive gas prevention |
The installation site must be free from corrosive gases such as acid gases and alkaline gases. For more information, see "Corrosive gas limit." |
EMI |
· If AC power is used, use a single-phase three-wire power receptacle with protection earth (PE) to filter interference from the power grid. · Keep the device far away from radio transmitting stations, radar stations, and high-frequency devices. · Use electromagnetic shielding, for example, shielded interface cables, when necessary. |
Cleanliness
Dust buildup on the chassis might cause electrostatic adsorption and dust corrosion, resulting in poor contact of metal connectors and contact points. This might shorten the device's lifetime and even cause device failure in the worst case. Table1-3 describes the switch requirement for cleanliness.
Table1-3 Switch requirement for cleanliness
Substance |
Particle diameter |
Concentration limit |
Dust particles |
≥ 0.5 µm |
≤ 1.8 × 107 particles/m3 |
To maintain cleanliness in the equipment room, follow these guidelines:
· Keep the equipment room away from pollution sources. Do not smoke, eat, or drink in the equipment room.
· Use double-layer glass in windows and seal doors and windows with dust-proof rubber strips. Use screen doors and window screens for doors and windows open to the outside and make sure the external windows are air tight.
· Use dustproof materials for floors, walls, and ceilings and use wallpaper or matt paint that does not produce powders.
· Clean the equipment room regularly and clean the air filters of the rack each month.
· Wear ESD clothing and shoe covers before entering the equipment room, keep the ESD clothing and shoe covers clean, and change them frequently.
Corrosive gas limit
Corrosive gases can accelerate corrosion and aging of metal components. Make sure the corrosive gases do not exceed the concentration limits as shown in Table1-4.
Table1-4 Corrosive gas concentration limits
Gas |
Average concentration (mg/m3) |
Maximum concentration (mg/m3) |
SO2 |
0.3 |
1.0 |
H2S |
0.1 |
0.5 |
Cl2 |
0.1 |
0.3 |
HCI |
0.1 |
0.5 |
HF |
0.01 |
0.03 |
NH3 |
1.0 |
3.0 |
O3 |
0.05 |
0.1 |
NOX |
0.5 |
1.0 |
CAUTION: As a best practice, control the corrosive gas concentrations in the equipment room at their average values. Make sure the corrosive gas concentrations do not exceed 30 minutes per day at their maximum values. |
To control corrosive gases, use the following guidelines:
· As a best practice, do not build the equipment room in a place with a high concentration of corrosive gases.
· Make sure the equipment room is not connected to sewer, vertical shaft, or septic tank pipelines and keep it far away from these pipelines. The air inlet of the equipment room must be away from such pollution sources.
· Use environmentally friendly materials to decorate the equipment room. Avoid using organic materials that contains harmful gases, such as sulfur or chlorine-containing insulation cottons, rubber mats, sound-proof cottons, and avoid using plasterboards with high sulfur concentration.
· Place fuel (diesel or gasoline) engines separately. Do not place them in the same equipment room with the device. Make sure the exhausted air of the engines will not flow into the equipment room or towards the air inlet of the air conditioners.
· Place batteries separately. Do not place them in the same room with the device.
· Employ a professional company to monitor and control corrosive gases in the equipment room regularly.
Before you install the switch, verify that the installation site meets the installation requirements. The switch can operate correctly in an A1 or A2 installation site. Availability issues might occur if you install the switch in an A3, B1, B2, or C installation site.
Category |
Definition |
Example |
A1: indoor controlled environment |
· Indoor environments where temperature and humidity are controlled. · Completely enclosed or shielded indoor environments. |
Central equipment rooms, IDC equipment rooms, mobile cabins with air conditioners, outdoor air conditioner cabinets, and heat exchanger cabinets. |
A2: indoor partially controlled environment |
· Indoor environments where temperature and humidity are partially controlled. · Incompletely enclosed or shielded places. · Places far from pollution sources. |
Simple equipment rooms, ordinary houses, garages, corridors, and direct ventilation cabinets far from pollution sources, houses without direct exposure to sunlight or rain, railway station platforms, and stadiums. |
A3: indoor uncontrolled environment |
· Indoor environments where temperature and humidity are uncontrolled. · Incompletely enclosed or shielded places. · Places near pollution sources. |
Simple equipment rooms, ordinary houses, garages, corridors, and direct ventilation cabinets near pollution sources, houses without direct exposure to sunlight or rain, railway station platforms, stadiums, uncleaned rooms after decoration, and rooms under decoration. |
B1: outdoor general environment |
· Unshielded places where the temperature and humidity are not controlled. · Places far from pollution sources. |
Completely exposed outdoor places far from pollution sources. |
B2: harsh environment |
· Unshielded places where the temperature and humidity are not controlled. · Sea environments or outdoor land environments near pollution sources. |
Islands, ships, and completely exposed outdoor places near pollution sources. |
C: special environments |
Special application environments |
Buried, underwater, or undersea environments and manholes. |
Table1-6 Pollution sources
Category |
Radius range |
Saline water areas such as oceans and saline lakes |
≤ 3.7 km (2.30 miles) |
Serious pollution sources such as metallurgic plants, coal mines, and heat and power plants |
≤ 3 km (1.86 miles) |
Medium pollution sources such as chemical factories, rubber plants, and electroplating factories |
≤ 2 km (1.24 miles) |
Light pollution sources, such as food factories, tanneries, and heating boilers |
≤ 1 km (0.62 miles) |
Table1-7 Requirements for power distribution or power supply environment
Item |
Requirements |
Preparation |
The power supply must be available before you install the switch. |
Voltage |
The voltage provided to the switch must be within the operating voltage range. For the operating voltage range, see S5580S-EI & S5580X-EI Switch Series Hardware Information and Specifications. |
Power receptacle and cables |
· If the power source is an AC power outlet, use a country-specific AC power cord. Make sure the PE wire of the AC power supply is grounded reliably. · If the power source is a DC distribution box, prepare DC power cords yourself. · Do not use the power cord provided with the switch on other devices. |
Laser safety
WARNING! Disconnected optical fibers or transceiver modules might emit invisible laser light. Do not stare into beams or view directly with optical instruments when the switch is operating. |
The switch is a Class 1 laser device.
Installation tools
No installation tools are provided with the switch. Prepare the following tools yourself as required.
· ESD wrist strap
· Flat-head screwdriver
· Phillips screwdriver
· Needle-nose pliers
· Diagonal pliers
· Crimping tool
· Marker
Installation accessories
Before installation, make sure you have all the required installation accessories. If an installation accessory is damaged or lost, purchase a new one as shown in Table1-8.
Table1-8 Installation accessories
Quantity |
Applicable device models |
Front mounting kit, including a pair of front mounting brackets and eight M4 screws |
1 set, provided |
All models |
M6 screw and cage nut |
User supplied |
All models |
Rubber feet |
Four, provided |
All models |
Grounding cable |
1, provided |
All models |
Grounding screw |
1, provided |
All models |
Power supply filler panel |
1, provided |
All models |
AC power cord The appearance and parameters for AC power cords vary depending on countries and regions. |
1, provided |
All models |
DB9-to-RJ45 console cable |
1, optional |
All models |
USB-to-RJ45 console cable |
1, optional |
All models |
2 Installing the switch
CAUTION: Keep the tamper-proof seal on a mounting screw on the chassis cover intact, and if you want to open the chassis, contact H3C for permission. Otherwise, H3C shall not be liable for any consequence. |
Figure2-1 Hardware installation flow
Figure2-2 Procedure for installing the switch in a 19-inch rack by using front mounting brackets
NOTE: If a rack shelf is available, you can put the switch on the rack shelf, slide the switch to an appropriate location, and attach the switch to the rack by using the mounting brackets. |
The switch has one mounting position near the ports and the other mounting position near the power supplies for the front mounting brackets. Select one position as needed.
To attach the front mounting brackets to the chassis:
1. Place the wide flange of the mounting bracket against the chassis side panel. Align the mounting bracket installation holes with the screw holes in the chassis.
¡ To install the mounting brackets at the port-side mounting position, see Figure2-3.
¡ To install the mounting brackets at the power supply-side mounting position, see Figure2-4.
2. Fasten the M4 screws to secure the mounting bracket to the switch.
3. Attach the front mounting bracket to the other side of the chassis in the same way.
Figure2-3 Attaching the front mounting brackets to the port-side mounting position
Figure2-4 Attaching the front mounting brackets to the power supply-side mounting position
1. Wear an ESD wrist strap and make sure it makes good skin contact and is reliably grounded.
2. Verify that the front mounting brackets have been securely attached to the switch chassis. For information about how to attach the front mounting brackets to the switch, see "Attaching the front mounting brackets to the switch."
3. Install cage nuts in the mounting holes in the rack posts.
4. One person supports the bottom of the switch, and moves the switch to an appropriate position based on the installation positions of the front mounting brackets.
5. The other person uses M6 screws and cage nuts to attach the mounting brackets to the rack and verifies that the brackets are level and secure.
Figure2-5 Mounting the switch in the rack
IMPORTANT: · Ensure 10 cm (3.9 in) of clearance around the chassis for heat dissipation. · Do not place heavy objects on the switch. |
If a standard 19-inch rack is not available, you can place you switch on a workbench.
To mount the switch on a workbench:
1. Verify that the workbench is sturdy and reliably grounded.
2. Place the switch with bottom up, and clean the round holes in the chassis bottom with dry cloth.
3. Attach the rubber feet to the four round holes in the chassis bottom.
4. Place the switch with upside up on the workbench.
Figure2-6 Mounting the switch on a workbench
WARNING! Correctly connecting the switch grounding cable is crucial to lightning protection, ESD, and EMI protection. For information about lightning protection, see H3C Network Devices Lightning Protection Guide. |
To protect against the following types of issues, use a grounding cable to connect the switch to the earthing facility at the installation site:
· Bodily injury from electric shocks.
· Device and power and data line damages.
· Electrical fires, lightning strokes, electromagnetic coupling interferences, and ESD damages.
You can ground the switch in one of the following ways, depending on the grounding conditions available at the installation site:
· Grounding the switch by using a grounding strip
· Grounding the switch with a grounding conductor buried in the earth ground
NOTE: The chassis views and power supply and grounding terminal positions in the following figures are for illustration only. |
WARNING! Connect the grounding cable to the grounding system in the equipment room. Do not connect it to a fire main or lightning rod. |
If a grounding strip is available at the installation site, use the grounding strip to ground the switch.
Connecting the grounding cable to the chassis
1. Remove the grounding screw from the grounding hole in the chassis.
2. Attach the grounding screw to the ring terminal of the grounding cable.
3. Use a screwdriver to fasten the grounding screw into the grounding hole.
Figure2-7 Attaching the grounding cable to the grounding hole of the switch
(1) Grounding screw |
(2) Ring terminal |
(3) Grounding sign |
(4) Grounding hole |
(5) Grounding cable |
Connecting the grounding cable to a grounding strip
1. Use needle-nose pliers to bend the bare metal part to a ring. Make sure the bended part can securely attached to a grounding post on the grounding strip.
2. Hook the bended part of the grounding cable to a grounding post and use the hex nut to secure the cable to the post.
Figure2-8 Connecting the grounding cable to a grounding strip
If the installation site does not have grounding strips, but earth ground is available, hammer a 2.5 m (8.20 ft) or longer angle iron or steel tube into the earth ground to act as a grounding conductor. Make sure a minimum of 0.7 m (2.30 ft) is left between the top of the grounding conductor and the ground. In cold areas, bury the grounding conductor below the frozen soil layer. In areas with thin soil or rocky gravel, determine the depth for burying the grounding conductor based on the actual condition.
If zinc-coated steel is used, the following dimensions requirements must be met:
· Angle iron—A minimum of 50 × 50 × 5 mm (1.97 × 1.97 × 0.20 in).
· Steel tube—A minimum of 3.5 mm (0.14 in) in thickness.
· Flat steel—A minimum of 40 × 4 mm (1.57 × 0.16 in).
· Round steel—A minimum of 10 mm (0.39 in).
Weld the yellow-green grounding cable to the angel iron or steel tube and treat the joint for corrosion protection.
Figure2-9 Grounding the switch by burying the grounding conductor into the earth ground
(2) Grounding cable |
(3) Earth |
(4) Joint |
(5) Grounding conductor |
· If you ground the switch with a grounding strip, perform the following tasks:
a. Use a multimeter to measure the resistance between the switch grounding terminal and grounding point, and make sure the resistance is less than 0.1W.
b. Use a grounding resistance tester to measure the grounding resistance of the grounding strip, and make sure the grounding resistance is less than 1W.
· If you ground the switch with a grounding conductor buried in the earth ground, perform the following tasks:
b. Use a grounding resistance tester to measure the grounding resistance of the angle iron in the ground, and make sure the grounding resistance is less than 10W. For locations with high soil resistivity, sprinkle some resistance reducer to reduce soil resistivity or replace soil around the grounding strip with soil with lower resistance.
For information about resistance measurement, see H3C Network Devices Lightning Protection Guide.
CAUTION: · The section is applicable to only switch models that support removable fan trays. · Before powering on the switch, make sure it has two fan trays of the same model installed. · Do not leave any slots empty when the switch is operating. · If one fan tray fails while the switch is operating, perform either of the following tasks: ¡ If the ambient temperature is not higher than 27°C (80.6°F), replace the fan tray within 24 hours and make sure the failed fan tray is in position before the replacement. ¡ If the ambient temperature is higher than 27°C (80.6°F), replace the fan tray immediately. · If both fan trays fail while the switch is operating, replace them within 2 minutes. |
The switch models that support removable fan trays came with empty fan tray slots. Choose fan tray models for the switch based on the ventilation requirement of the site. The air flow direction varies by fan tray model.
· The FAN-40B-1-F or LSPM1FANSA-SN fan tray blows air from the power supply side to the port side. The fan tray handle is blue.
· The FAN-40F-1-F or LSPM1FANSB-SN fan tray draws air from the port side to the power supply side. The fan tray handle is red.
For more information about the fan trays, see technical specifications in S5580S-EI & S5580X-EI Switch Series Hardware Information and Specifications.
Installing a fan tray
CAUTION: To prevent damage to the fan tray or the connectors in the chassis, insert the fan tray gently. If you encounter a hard resistance while inserting the fan tray, pull out the fan tray and insert it again. |
To install a fan tray:
2. Unpack the fan tray and verify that the fan tray model is correct.
3. Grasping the two handles of the fan tray with the side marked TOP facing up, slide the fan tray along the guide rails into the slot until the fan tray seats in the slot and has a firm contact with the backplane.
Figure2-10 Installing a fan tray
Removing a fan tray
WARNING! · To avoid bodily injury, and disturbing the dynamic balance of the fan tray and causing loud noises, do not touch the rotation axis, any bare wires, fan blades, or terminals on the fan tray. · Do not place the fan tray in a moist place. Prevent liquid from entering the fan tray. Put the removed fan tray in an antistatic bag. · Fan trays with faulty internal wiring and components require maintenance from maintenance engineers. Do not disassemble the faulty fan trays without permission. |
To remove a fan tray:
2. As shown by callout 1 in Figure2-11, grasping the two handles of the fan tray, pull out the fan tray slowly along the guide rails.
3. Put the removed fan tray in an antistatic bag.
Figure2-11 Removing a fan tray
Table2-2 Power supply installation/removal method
Power supply model |
Installation/removal method |
CA-70A12 PSR75-12A PSR180-12D-B PSR180-12A-F PSR180-12A-B |
PSR600-54A-B PSR920-54A-B PSR1600-54A-B |
The switch came with power supply slot PWR1 empty and power supply slot PWR2 installed with a filler panel. You can install one or two power supplies for the switch as required. For the power supplies available for the switch and their specifications, see technical specifications in the hardware information and specifications for the switch.
CAUTION: · Provide a circuit breaker for each power supply and make sure the circuit breaker is off before installation. · To prevent damage to the power supply or the connectors on the backplane, insert the power supply gently. If you encounter a hard resistance when inserting the power supply, pull out the power supply and insert it again. |
To avoid device damage and bodily injury, follow the procedures in Figure2-12 and Figure2-13 to install and replace a power supply.
Figure2-12 Installation procedure
This section applies to the CA-70A12, PSR75-12A, PSR180-12D-B, PSR180-12A-B, and PSR180-12A-F power supplies, which use similar installation and removal procedures. The following uses the PSR75-12A power supply as an example.
Installing a power supply
2. Unpack the power supply and verify that the power supply model is as required.
3. Remove the filler panel (if any) from the target slot.
Use a Phillips screwdriver to loosen the mounting screws on the filler panel, and then remove the filler panel.
Figure2-14 Removing the filler panel
4. Orient the power supply with the lettering on it upright. Grasping the power supply handle with one hand and supporting its bottom with the other, slide the power supply slowly along the guide rails into the slot. See callout 1 in Figure2-15.
5. Fasten the captive screws on the power supply with a Phillips screwdriver to secure the power supply in the chassis. See callout 2 in Figure2-15.
Use a torque of 5 kgf-cm (0.49 Nm) to fasten the captive screws on the power supply.
Figure2-15 Installing a PSR75-12A power supply
Removing a power supply
2. Power off the power supply and remove the power cord.
3. Loosen the captive screws of the power supply with a Phillips screwdriver until they are completely disengaged.
4. Grasping the power supply handle with one hand, pull it part way out. Supporting the bottom with the other hand, pull the power supply slowly out of the slot along the guide rails.
5. Put the removed power supply on an antistatic mat or in its original package.
6. If you are not to install a new power supply, install a filler panel in the slot.
Figure2-16 Removing a PSR75-12A power supply
This section applies to the PSR600-54A-B, PSR920-54A-B, and PSR1600-54A-B power supplies, which use similar installation and removal procedures. The following uses the PSR600-54A-B power supply as an example.
Keep the removed power supply filler panel and power supply package secure for future use.
Figure2-17 Removing the filler panel
4. Orient the power supply with the lettering on it upright. Grasping the power supply handle with one hand and supporting the power supply bottom with the other, slide the power supply slowly into the slot along the guide rails until you hear a click.
Follow the forward inertia of the power supply when inserting it into the chassis, and make sure the power supply has firm contact with the connectors on the backplane.
Figure2-18 Installing a PSR920-54A-B power supply
2. Turn off the circuit breaker for the power supply.
3. Release the releasable cable tie and disconnect the power cord.
4. Press the latch on the power supply towards the handle direction and pull the power supply part way out of the slot, as shown in Figure2-19.
5. Grasping the power supply handle with one hand and supporting the power supply bottom with the other, pull the power supply slowly out of the slot along the guide rails.
6. Put the removed power supply on an antistatic mat or in its original package.
Figure2-19 Removing a PSR920-54A-B power supply
7. If you are not to install a new power supply, install a filler panel in the slot.
CAUTION: · Provide a circuit breaker for each power cord. · Before connecting the power cord, make sure the circuit breaker on the power cord is turned off. |
Table2-3 Power cord connection procedures at a glance
Available power source |
Connection procedure reference |
PSR75-12A CA-70A12 PSR180-12A-F PSR180-12A-B |
AC power source |
Connecting the power cord for a PSR75-12A, CA-70A12, PSR180-12A-F, or PSR180-12A-B power supply |
AC power source |
Connecting the power cord for a PSR600-54A-B, PSR920-54A-B, or PSR1600-54A-B power supply |
PSR180-12D-B |
–48 VDC power source in the equipment room |
RPS1600-A |
The power cord connection procedure is the same for the PSR75-12A, CA-70A12, PSR180-12A-F, and PSR180-12A-B power supplies. The following uses a CA-70A12 power supply as an example.
To connect the power cord for a CA-70A12 power supply:
2. Attach the power cord retainer clip into the two holes next to the AC-input power receptacle on the power supply, and pull the retainer clip leftwards (see Figure2-20).
3. Connect the female connector of the AC power cord supplied with the power supply to the power receptacle (see Figure2-20).
4. Pull the retainer clip rightwards to secure the connector to the AC-input power receptacle (see Figure2-20).
5. Connect the other end of the power cord to an AC power source.
Figure2-20 Connecting the power cord for a CA-70A12 power supply
The power cord connection procedure is the same for the PSR600-54A-B, PSR920-54A-B, and PSR1600-54A-B power supplies. The following uses a PSR920-54A-B power supply as an example.
To connect the power cord for a PSR920-54A-B power supply:
2. Plug the female connector of the power cord into the power receptacle on the power supply.
3. Use a releasable cable tie to secure the power cord to the handle of the power supply.
4. Connect the other end of the power cord to an external power source.
Figure2-21 Connecting the power cord for a PSR920-54A-B power supply
CAUTION: · To use a –48 VDC power source to supply power to the power supply, use the DC power cord supplied with the power supply. To connect to an H3C recommended RPS, use a power cord compatible with the RPS. · To connect a DC power cord to a –48 VDC power source, identify the positive (+) and negative (-) marks on the two wires of the power cord to avoid connection mistakes. |
To connect the power cord for a PSR180-12D-B power supply:
2. Correctly orient the plug at one end of the cable with the power receptacle on the power supply, and then insert the plug into the power receptacle (see callout 1 in Figure2-22).
The DC power receptacle and DC power cord connector are designed in a structure to prevent misalignment. If you cannot insert the plug into the receptacle, re-orient the plug rather than use excessive force to push it in.
3. Fasten the screws on the plug with a flat-head screwdriver to secure the plug in the power receptacle (see callout 2 in Figure2-22).
4. Connect the other end of the power cord to a –48 VDC power source or an RPS.
Figure2-22 Connecting the power cord for a PSR180-12D-B power supply
CAUTION: · Do not touch the surface-mounted components directly with your hands. · Do not use excessive force when you install or remove an expansion card. · You can install or remove an expansion card when the switch is operating correctly. Do not install or remove an expansion card on a starting switch. |
The S5580X-HI switch series provides an expansion slot at the rear. For the expansion cards available for the switch, see technical specifications in the hardware information and specifications for the switch.
The installation and removal procedures are similar for the expansion cards. This section uses the LSWM2QP2P card (with an ejector lever) and the LSPM6FWD card (without an ejector lever) as examples.
Installing an expansion card
2. Use a Phillips screwdriver to remove the mounting screws on the filler panel over the expansion slot, and then remove the filler panel.
Keep the removed the filler panel secure for future use.
Figure2-23 Removing the filler panel
3. Unpack the expansion card.
4. If the expansion card has an ejector lever, follow these steps to install it:
a. Open the ejector lever, as shown by callout 1 in Figure2-24.
b. Gently slide the expansion card into the slot along the guide rails until the expansion card has good contact with the chassis, as shown by callout 2 in Figure2-24.
c. Close the ejector lever, as shown by callout 3 in Figure2-25.
d. Use a Phillips screwdriver to fasten the mounting screw on the expansion card to secure it in the slot, as shown by callout 4 in Figure2-25.
5. If the expansion card does not have an ejector lever, follow these steps to install it:
a. Gently slide the expansion card into the slot along the guide rails until the expansion card has good contact with the chassis, as shown by callout 1 in Figure2-26.
b. Use a Phillips screwdriver to fasten the mounting screw on the expansion card to secure it in the slot, as shown by callout 2 in Figure2-26.
6. If you are not to install a new expansion card, install a filler panel in the slot to prevent dust and ensure good ventilation in the switch.
Figure2-24 Installing an LSWM2QP2P expansion card (1)
Figure2-25 Installing an LSWM2QP2P expansion card (2)
Figure2-26 Installing an LSPM6FWD expansion card
Figure2-27 LSPM6FWD firewall module installed in the switch
NOTE: · An LSPM6FWD firewall module (including its handle) adds 75 mm (2.95 in) to the chassis depth. · An LSWM2EC EPS scanner module (including its handle) adds 76 mm (2.99 in) to the chassis depth. |
Removing an expansion card
2. Use a Phillips screwdriver to remove the mounting screw on the expansion card.
3. If the expansion card has an ejector lever, open the ejector lever. Skip this step if the expansion card does not have an ejector lever.
4. Gently pull the expansion card out of the slot along the guide rails.
Verifying the installation
After you complete the installation, verify that:
· There is enough space for heat dissipation around the switch, and the rack or workbench is stable.
· The grounding cable is securely connected.
· The correct power source is used.
· The power cords are correctly connected.
· All the interface cables are cabled indoors. If any cable is routed outdoors, verify that the socket strip with lightning protection and lightning arresters for network ports have been correctly connected.
NOTE: For information about lightning protection for the switch, see H3C Lightning Protection Guide. |
The switch provides a serial console port.
In Figure3-1, the switch is connected to a configuration terminal (PC as an example) from the serial console port.
Figure3-1 Connecting the switch to a configuration terminal
As shown in Figure3-1, two types of serial console cables can be used for connecting the switch to a configuration terminal. The switch is not provided with a serial console cable.
Table3-1 Connection methods and console cables
Connection method |
Console cable type |
Configuration terminal-side connector |
Switch-side connector |
Using the serial console port for connection |
DB-9 female connector |
RJ-45 connector |
USB connector |
RJ-45 connector |
The signal pinout for the RJ-45 connector of a serial console cable varies by vendor. To avoid abnormal configuration terminal display, use a serial console cable provided by H3C. For more information, see Table1-8. To prepare a serial console cable yourself, make sure the signal pinout for the RJ-45 connector is the same as that shown in Table3-2.
CAUTION: Follow these guidelines when you connect a DB9-to-RJ45 console cable: · Identify the mark on the serial console port and make sure you are connecting to the correct port. · The serial ports on PCs do not support hot swapping. To connect a PC to an operating switch, first connect the PC end. To disconnect a PC from an operating switch, first disconnect the switch end. |
A DB9-to-RJ45 serial console cable is an 8-core shielded cable, with a crimped RJ-45 connector at one end for connecting to the serial console port of the switch, and a DB-9 female connector at the other end for connecting to the serial port on a configuration terminal.
Figure3-2 DB9-to-RJ45 console cable
Table3-2 DB9-to-RJ45 console cable signal pinout
RJ-45 |
Signal |
DB-9 |
Signal |
1 |
RTS |
8 |
CTS |
2 |
DTR |
6 |
DSR |
3 |
TXD |
2 |
RXD |
4 |
SG |
5 |
SG |
5 |
SG |
5 |
SG |
6 |
RXD |
3 |
TXD |
7 |
DSR |
4 |
DTR |
8 |
CTS |
7 |
RTS |
To connect the switch to a configuration terminal (for example, a PC) by using a DB9-to-RJ45 console cable:
1. Plug the DB-9 female connector of the DB9-to-RJ45 console cable to the serial port on the PC.
2. Connect the RJ-45 connector to the serial console port on the switch.
IMPORTANT: · To use a USB-to-RJ45 console cable to connect the switch to a configuration terminal, first download and install the USB-to-RJ45 console driver on the configuration terminal and then connect the USB-to-RJ45 console cable to the configuration terminal. · If you have connected a USB-to-RJ45 console cable to the configuration terminal before installing the driver, remove and reconnect the USB-to-RJ45 console cable to the configuration terminal after driver installation. |
For information about the signal pinout for the RJ-45 connector of a USB-to-RJ45 console cable, see Table3-2.
The following installs the driver on the Windows system. To install the driver on other operating systems, see the installation guide in the driver compression package named by using the corresponding operating system.
To connect the switch to a configuration terminal by using a USB-to-RJ45 console cable:
1. Click the following link, or copy it to the address bar on your browser and download the USB-to-RJ45 console driver.
http://www.h3c.com/en/home/USB_to_RJ45_Console/
2. View the TXT file Read me in the Windows folder to check whether the Windows system of the configuration terminal supports the driver.
3. If the Windows system supports the driver, install PL23XX-M_LogoDriver_Setup_v200_20190815.exe.
4. Click Next on the welcome page of the driver installation wizard.
Figure3-3 Driver installation wizard
5. Click Finish after the drive installation is completed.
Figure3-4 Finishing the driver installation
6. Connect the standard USB connector of the cable to the USB port of the configuration terminal.
7. Connect the RJ-45 connector of the cable to the console port of the switch.
Setting terminal parameters
To configure and manage the switch through the console port, you must run a terminal emulator program, such as TeraTermPro, on your configuration terminal. You can use the emulator program to connect a network device, a Telnet site, or an SSH site. For more information about the terminal emulator programs, see the user guides for these programs.
Configure the terminal parameters as follows:
· Bits per second—9600.
· Data bits—8.
· Stop bits—1.
· Parity—None.
· Flow control—None.
Powering on the switch
Before powering on the switch, verify that the following conditions are met:
· The power cord is correctly connected.
· The input power voltage meets the requirement of the switch.
· The console cable is correctly connected.
· The configuration terminal (a PC, for example) has started, and its serial port settings are consistent with the console port settings on the switch.
During the startup process, you can access Boot ROM menus to perform tasks such as software upgrade and file management. The Boot ROM interface and menu options differ with software versions. For more information about Boot ROM menu options, see the software-matching release notes for the device.
After the startup completes, you can access the CLI to configure the switch.
For more information about the configuration commands and CLI, see the configuration guides and command references for the switch series.
Power supply failure
You can determine the power supply operating status by examining the power supply LEDs PWR1 and PWR2 on the switch front panel. For descriptions about the PWR1 and PWR2 LEDs, see LEDs in S5580S-EI & S5580X-EI Switch Series Hardware Information and Specifications.
Symptom
A power supply LED on the front panel of the switch is not steady green.
Solution
To resolve the issue:
1. Verify that the power supply model is as required by the switch.
2. Verify that the power supply is installed correctly in the switch.
3. Verify that the power cord is connected correctly.
4. Verify that the external power source is operating correctly.
5. Verify that the electrical outlet is operating correctly.
6. Verify that the operating temperature of the switch is in an acceptable range and the power supply has good ventilation.
7. If the power supply needs to be replaced, see "Installing and removing power supplies" to replace the power supply.
8. If the issue persists, contact H3C Support.
Removable fan tray failure
You can determine the removable fan tray operating status by examining the system status LED (SYS) on the switch and the fan tray alarm LED on the fan tray. For descriptions about the LEDs, see LEDs in S5580S-EI & S5580X-EI Switch Series Hardware Information and Specifications.
Symptom
The system status LED (SYS) on the switch and the fan tray alarm LED indicate a fan tray failure.
Solution
CAUTION: Before powering on the switch, make sure it has two fan trays of the same model installed. |
· If both fan trays fail while the switch is operating, replace them within 2 minutes while the switch is operating.
For how to replace a fan tray, see "Installing and removing fan trays."
Configuration terminal issues
If the configuration environment setup is correct, the configuration terminal displays booting information when the switch is powered on. If the setup is incorrect, the configuration terminal displays nothing or garbled text.
Symptom
The configuration terminal does not have display when the switch is powered on.
Solution
1. Verify that the power system is operating correctly.
2. Verify that the console cable has been connected correctly.
3. Verify that the following settings are configured for the terminal:
¡ Baud rate—9600.
¡ Data bits—8.
¡ Parity—None.
¡ Stop bits—1.
¡ Flow control—None.
4. Verify that the console cable is not faulty.
5. If the issue persists, contact H3C Support.
Symptom
The configuration terminal displays garbled text.
Solution
1. Verify that the following settings are configured for the terminal:
¡ Baud rate—9600.
¡ Data bits—8.
¡ Parity—None.
¡ Stop bits—1.
2. If the issue persists, contact H3C Support.