Configuring PoE

About PoE

Power over Ethernet (PoE) enables a network device to supply power to terminals over twisted pair cables.

PoE system

As shown in Figure 1, a PoE system includes the following elements:

·     PoE power supply—A PoE power supply provides power for the entire PoE system.

·     PSE—A power sourcing equipment (PSE) supplies power to PDs. PSE devices are classified into single-PSE devices and multiple-PSE devices.

¡     A single-PSE device has only one piece of PSE firmware.

¡     A multiple-PSE device has multiple PSEs. A multiple-PSE device uses PSE IDs to identify different PSEs. To view the mapping between the ID and slot number of a PSE, execute the display poe device command.

The device is a multiple-PSE device.

·     PI—A power interface (PI) is a PoE-capable Ethernet interface on a PSE.

·     PD—A powered device (PD) receives power from a PSE. PDs include IP telephones, APs, portable chargers, POS terminals, and Web cameras. You can also connect a PD to a redundant power source for reliability.

Figure 1 PoE system diagram

Protocols and standards

·     802.3af-2003, IEEE Standard for Information Technology - Telecommunications and Information Exchange Between Systems - Local and Metropolitan Area Networks - Specific Requirements - Part 3: Carrier Sense Multiple Access with Collision Detection (CSMA/CD) Access Method and Physical Layer Specifications - Data Terminal Equipment (DTE) Power Via Media Dependent Interface (MDI)

·     802.3at-2009, IEEE Standard for Information technology-- Local and metropolitan area networks-- Specific requirements-- Part 3: CSMA/CD Access Method and Physical Layer Specifications Amendment 3: Data Terminal Equipment (DTE) Power via the Media Dependent Interface (MDI) Enhancements

Restrictions and guidelines: PoE configuration

You can configure settings for a PI through either of the following ways:

·     Configure the settings directly on the PI.

·     Configure a PoE profile and apply it to the PI. If you apply a PoE profile to multiple PIs, these PIs have the same PoE features. If you connect a PD to another PI, you can apply the PoE profile of the original PI to the new PI. This method relieves the task of configuring PoE on the new PI.

You can only use one way to configure a parameter for a PI. To use the other way to reconfigure a parameter, you must first remove the original configuration.

You must use the same configuration method for the poe max-power max-power and poe priority { critical | high | low } commands.

If a PI fails to supply power to a device connected to it, identify whether the device is a PD. If it is a PD, enable nonstandard PD protection for the device.

PoE configuration tasks at a glance

To configure PoE, perform the following tasks:

1.     Enabling PoE

a.     Enabling PoE for a PI

2.     (Optional.) Configuring PoE delay

3.     (Optional.) Disabling PoE on shutdown interfaces

4.     (Optional.) Allowing inrush currents drawn by PDs

5.     (Optional.) Enabling PI power cycling upon a system warm reboot

6.     (Optional.) Configuring PD detection

¡     Enabling nonstandard PD detection

7.     (Optional.) Configuring the PoE power

¡     Configuring the maximum PI power

8.     (Optional.) Configuring the PoE priority policy

¡     Configuring the PI priority policy

9.     (Optional.) Configuring PoE monitoring

¡     Configuring PSE power monitoring

10.     (Optional.) Configuring a PI by using a PoE profile

To use a PoE profile to enable PoE and configure the priority and maximum power for a PI, see "Configuring a PI by using a PoE profile."

11.     (Optional.) Upgrading PSE firmware in service

Prerequisites for configuring PoE

Before you configure PoE, make sure the PoE power supply and PSEs are operating correctly.

Enabling PoE

Enabling PoE for a PI

About this task

After you enable PoE for a PI, the PI supplies power to the connected PD if the PI will not result in PSE power overload. PSE overload occurs when the sum of the power consumption of all PIs exceeds the maximum power of the PSE.

If the PI will result in PSE power overload, the following restrictions apply:

·     If the PI priority policy is not enabled, the PI does not supply power to the connected PD.

·     If the PI priority policy is enabled, whether the PDs can be powered depends on the priority of the PI.

For more information about the PI priority policy, see "Configuring the PI priority policy."

Restrictions and guidelines

A PI can supply power to a PD only when the PI and PD use the same power transmission mode.

Procedure

1.     Enter system view.

system-view

2.     Enter PI view.

interface interface-type interface-number

3.     (Optional.) Configure a description for the PD connected to the PI.

poe pd-description text

By default, no description is configured for the PD connected to the PI.

4.     Enable PoE for the PI.

poe enable

By default, when the device starts up with the initial configuration, PoE is disabled on PIs. When the device starts up with the factory defaults, PoE is enabled on PIs.

For more information about the initial configuration and factory defaults, see configuration file management in Fundamentals Configuration Guide.

Configuring PoE delay

About this task

By default, the device executes the poe enable command and supplies power to an interface immediately when any one of the following conditions is met:

·     The poe enable command is configured.

·     The device reboots with the poe enable command in the configuration file.

·     The interface comes up and the PoE module resumes PoE power supply to the interface.

This task creates a PoE delay timer after the poe enable command is executed and allows the PoE module to supply power to the PI only after the timer expires.

Restrictions and guidelines

The undo poe enable command is executed immediately upon configuration and is not affected by this task.

Procedure

1.     Enter system view.

system-view

2.     Enable PoE delay.

poe power-delay time

By default, PoE delay is disabled.

Disabling PoE on shutdown interfaces

About this task

By default, the device continues supplying power to an interface after the interface is shut down by the shutdown command or by an upper layer module such as monitor link. As a result, the PD connected to the shutdown interface operates continuously but fails to access the network.

This task disables the PoE module from supplying power to an interface after the interface is shut down. After the interface comes up or you disable this task, the PoE module resumes power supply to the interface.

Restrictions and guidelines

The task does not power off an interface that has been shut down but is supplying power to a PD.

Procedure

1.     Enter system view.

system-view

2.     Disable PoE on shutdown interfaces.

poe track-shutdown

By default, PoE is not disabled on shutdown interfaces.

Allowing inrush currents drawn by PDs

About this task

Inrush current might occur at PD startup and trigger PSE self-protection, As a result, the PSE stops supplying power to the PDs. To continue power supply to the PDs, configure this feature to allow inrush current drawn by PDs.

IEEE 802.3af and IEEE 802.3at define specifications for inrush current.

Restrictions and guidelines

CAUTION

CAUTION:

Inrush current might damage device components. Use this feature with caution.

 

Procedure

1.     Enter system view.

system-view

2.     Enter PI view.

interface interface-type interface-number

3.     Allow inrush current drawn by PDs.

poe high-inrush enable pse pse-id

By default, inrush current drawn by PDs is not allowed.

Enabling PI power cycling upon a system warm reboot

About this task

During the system warm reboot process (upon execution of the reboot command), the PIs continue supplying power to the PDs but data connections between the PDs and the device are interrupted. After the system reboots, PDs might not re-initiate data connections with the device. Power cycling PIs upon a system warm reboot allows the PDs to re-establish data connections with the device after a warm reboot.

Procedure

1.     Enter system view.

system-view

2.     Enter PI power cycling upon a system warm reboot.

poe reset enable

By default, PI power cycling upon a system warm reboot is disabled.

Configuring PD detection

Enabling nonstandard PD detection

About this task

PDs are classified into standard PDs and nonstandard PDs. Standard PDs are compliant with IEEE 802.3af and IEEE 802.3at. A PSE supplies power to a nonstandard PD only after nonstandard PD detection is enabled.

The device supports PSE-based and PI-based nonstandard PD detection. Enabling nonstandard PD detection for a PSE enables this feature for all PIs on the PSE. As a best practice for disabling nonstandard PD detection for all PIs successfully in one operation, disable this feature in both system view and interface view.

Procedure

1.     Enter system view.

system-view

2.     Enable nonstandard PD detection. Choose one option as needed.

¡     Enable nonstandard PD detection for the PSE.

poe legacy enable pse pse-id

By default, nonstandard PD detection is disabled for a PSE.

¡     Execute the following commands in sequence to enable nonstandard PD detection for a PI:

interface interface-type interface-number

poe legacy enable

By default, nonstandard PD detection is disabled for a PI.

Configuring the PoE power

Configuring the maximum PI power

About this task

The maximum PI power is the maximum power that a PI can provide to the connected PD. If the PD requires more power than the maximum PI power, the PI does not supply power to the PD.

Procedure

1.     Enter system view.

system-view

2.     Enter PI view.

interface interface-type interface-number

3.     Configure the maximum power for the PI.

poe max-power max-power

By default, the maximum PI power is 35000 milliwatts.

Configuring the PoE priority policy

Configuring the PI priority policy

About this task

The PI priority policy enables the PSE to perform priority-based power allocation to PIs when PSE power overload occurs. The priority levels for PIs are critical, high, and low in descending order.

When PSE power overload occurs, the PSE supplies power to PDs as follows:

·     If the PI priority policy is disabled, the PSE supplies power to PDs depending on whether you have configured the maximum PSE power.

¡     If you have configured the maximum PSE power, the PSE does not supply power to the newly-added or existing PD that causes PSE power overload.

¡     If you have not configured the maximum PSE power, the PoE self-protection mechanism is triggered. The PSE stops supplying power to all PDs.

·     If the PI priority policy is enabled, the PSE supplies power to PDs as follows:

¡     If a PD being powered causes PSE power overload, the PSE stops supplying power to the PD.

¡     If a newly-added PD causes PSE power overload, the PSE supplies power to PDs in priority descending order of the PIs to which they are connected. If the newly-added PD and a PD being powered have the same priority, the PD being powered takes precedence. If multiple PIs being powered have the same priority, the PIs with smaller IDs takes precedence.

Restrictions and guidelines

Before you configure a PI with critical priority, make sure the remaining power from the maximum PSE power minus the maximum powers of the existing PIs with critical priority is greater than maximum power of the PI.

Configuration for a PI whose power is preempted remains unchanged.

Procedure

1.     Enter system view.

system-view

2.     Enable the PI priority policy.

poe pd-policy priority

By default, the PI priority policy is disabled.

3.     Enter PI view.

interface interface-type interface-number

4.     (Optional.) Configure a priority for the PI.

poe priority { critical | high | low }

By default, the priority for a PI is low.

Configuring PoE monitoring

Configuring PSE power monitoring

About this task

The system monitors PSE power utilization and sends notification messages when PSE power utilization exceeds or drops below the threshold. If PSE power utilization crosses the threshold multiple times in succession, the system sends notification messages only for the first crossing. For more information about the notification message, see "Configuring SNMP."

Procedure

1.     Enter system view.

system-view

2.     Configure a power alarm threshold for a PSE.

poe utilization-threshold value pse pse-id

By default, the power alarm threshold for a PSE is 80%.

Configuring a PI by using a PoE profile

Restrictions and guidelines

To modify a PoE profile applied on a PI, first remove the PoE profile from the PI.

You can configure a PI either on the PI or by using a PoE profile. The poe max-power max-power and poe priority { critical | high | low } commands must be configured using the same method.

 

Configuring a PoE profile

1.     Enter system view.

system-view

2.     Create a PoE profile and enter its view.

poe-profile profile-name [ index ]

By default, no PoE profiles exist.

3.     Enable PoE.

poe enable

By default, PoE is disabled.

4.     (Optional.) Configure the maximum PI power.

poe max-power max-power

By default, the maximum PI power is 35000 W.

5.     (Optional.) Configure a PI priority.

poe priority { critical | high | low }

The default priority is low.

This command takes effect only after the PI priority policy is enabled.

Applying a PoE profile

Restrictions and guidelines

You can apply a PoE profile to multiple PIs in system view or a single PI in PI view. If you perform the operation in both views for the same PI, the most recent operation takes effect.

You can apply only one PoE profile to a PI.

Applying a PoE profile in system view

1.     Enter system view.

system-view

2.     Apply a PoE profile to PIs.

apply poe-profile { index index | name profile-name } interface interface-range

By default, a PoE profile is not applied to a PI.

Applying a PoE profile in PI view

1.     Enter system view.

system-view

2.     Enter PI view.

interface interface-type interface-number

3.     Apply the PoE profile to the interface.

apply poe-profile { index index | name profile-name }

By default, a PoE profile is not applied to a PI.

Upgrading PSE firmware in service

About this task

You can upgrade the PSE firmware in service in the following modes:

·     Refresh mode—Updates the PSE firmware without deleting it. You can use the refresh mode in most cases.

·     Full mode—Deletes the current PSE firmware and reloads a new one. Use the full mode if the PSE firmware is damaged and you cannot execute any PoE commands.

Restrictions and guidelines

If the PSE firmware upgrade fails because of interruption such as a device reboot, you can restart the device and upgrade it in full mode again. After the upgrade, restart the device manually for the new PSE firmware to take effect.

Procedure

1.     Enter system view.

system-view

2.     Upgrade the PSE firmware in service.

poe update { full | refresh } filename pse pse-id

Display and maintenance commands for PoE

Execute display commands in any view.

 

Task

Command

Display brief PSE information.

display poe device [ slot slot-number ]

Display the power supplying information for the specified PI.

display poe interface [ interface-type interface-number ]

Display power information for PIs.

display poe interface power [ interface-type interface-number ]

Display detailed PSE information.

display poe pse [ pse-id ]

Display the power supplying information for all PIs on a PSE.

display poe pse pse-id interface

Display power information for all PIs on a PSE.

display poe pse pse-id interface power

Display all information about the PoE profile.

display poe-profile [ index index | name profile-name ]

Display all information about the PoE profile applied to the specified PI.

display poe-profile interface interface-type interface-number

PoE configuration examples

Example: Configuring PoE

Network configuration

As shown in Figure 2, the device has PSEs 4 and 7, in slot 1 and 2, respectively. Configure PoE to meet the following requirements:

·     The device supplies power to IP phones and APs.

·     IP phone B takes precedence to receive power when PSE power overload occurs.

·     Power supplied to AP B does not exceed 9000 milliwatts.

Figure 2 Network diagram

Procedure

# Enable the PI priority policy.

<PSE> system-view

[PSE] poe pd-policy priority

# Enable PoE on GigabitEthernet 1/0/1 and GigabitEthernet 2/0/1.

[PSE] interface gigabitethernet 1/0/1

[PSE-GigabitEthernet1/0/1] poe enable

[PSE-GigabitEthernet1/0/1] quit

[PSE] interface gigabitethernet 2/0/1

[PSE-GigabitEthernet2/0/1] poe enable

[PSE-GigabitEthernet2/0/1] quit

# Enable PoE on GigabitEthernet 1/0/2, and set its power priority to critical.

[PSE] interface gigabitethernet 1/0/2

[PSE-GigabitEthernet1/0/2] poe enable

[PSE-GigabitEthernet1/0/2] poe priority critical

[PSE-GigabitEthernet1/0/2] quit

# Enable PoE on GigabitEthernet 2/0/2, and set its maximum power to 9000 milliwatts.

[PSE] interface gigabitethernet 2/0/2

[PSE-GigabitEthernet2/0/2] poe enable

[PSE-GigabitEthernet2/0/2] poe max-power 9000

Verifying the configuration

# Verify that the device is supplying power correctly to the IP phones and APs, and the IP phones and APs are operating correctly.

Troubleshooting PoE

Failure to set the priority of a PI to critical

Symptom

Power supply priority configuration for a PI failed.

Solution

To resolve the issue:

1.     Identify whether the remaining guaranteed power of the PSE is lower than the maximum power of the PI. If it is, increase the maximum PSE power or reduce the maximum power of the PI.

2.     Identify whether the priority has been configured through other methods. If the priority has been configured, remove the configuration.

3.     If the issue persists, contact H3C Support.

Failure to apply a PoE profile to a PI

Symptom

PoE profile application for a PI failed.

Solution

To resolve the issue:

1.     Identify whether some settings in the PoE profile have been configured. If they have been configured, remove the configuration.

2.     Identify whether the settings in the PoE profile meet the requirements of the PI. If they do not, modify the settings in the PoE profile.

3.     Identify whether another PoE profile is already applied to the PI. If it is, remove the application.

4.     If the issue persists, contact H3C Support.

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Intelligent Storage
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
  • Technical Blogs
All Support
  • Become A Partner
  • Partner Policy & Program
  • Global Learning
  • Partner Sales Resources
  • Partner Business Management
  • Service Business
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us