11-Network Management and Monitoring Configuration Guide
HomeSupportSwitchesFS5100-EI SeriesConfigure & DeployConfiguration GuidesH3C E500C-F & FS5100-EI Configuration Guides-R63xx-6W10011-Network Management and Monitoring Configuration Guide
08-CWMP configuration
08-CWMP configuration 393.88 KB
Configuring CWMP
About CWMP
CPE WAN Management Protocol (CWMP), also called "TR-069," is a DSL Forum technical specification for remote management of network devices.
The protocol was initially designed to provide remote autoconfiguration through a server for large numbers of dispersed end-user devices in a network. CWMP can be used on different types of networks, including Ethernet.
CWMP network framework
Figure 1 shows a basic CWMP network framework.
Figure 1 CWMP network framework
A basic CWMP network includes the following network elements:
·     ACS—Autoconfiguration server, the management device in the network.
·     CPE—Customer premises equipment, the managed device in the network.
·     DNS server—Domain name system server. CWMP defines that the ACS and the CPE use URLs to identify and access each other. DNS is used to resolve the URLs.
·     DHCP server—Assigns ACS attributes along with IP addresses to CPEs when the CPEs are powered on. DHCP server is optional in CWMP. With a DHCP server, you do not need to configure ACS attributes manually on each CPE. The CPEs can contact the ACS automatically when they are powered on for the first time.
The device is operating as a CPE in the CWMP framework.
Basic CWMP functions
You can autoconfigure and upgrade CPEs in bulk from the ACS.
Autoconfiguration
You can create configuration files for different categories of CPEs on the ACS. Based on the device models and serial numbers of the CPEs, the ACS verifies the categories of the CPEs and issues the associated configuration to them.
The following are methods available for the ACS to issue configuration to the CPE:
·     Transfers the configuration file to the CPE, and specifies the file as the next-startup configuration file. At a reboot, the CPE starts up with the ACS-specified configuration file.
·     Runs the configuration in the CPE's RAM. The configuration takes effect immediately on the CPE. For the running configuration to survive a reboot, you must save the configuration on the CPE.
CPE software management
The ACS can manage CPE software upgrade.
When the ACS finds a software version update, the ACS notifies the CPE to download the software image file from a specific location. The location can be the URL of the ACS or an independent file server.
If the CPE successfully downloads the software image file and the file is validated, the CPE notifies the ACS of a successful download. If the CPE fails to download the software image file or the file is invalidated, the CPE notifies the ACS of an unsuccessful download.
Data backup
The ACS can require the CPE to upload a configuration file or log file to a specific location. The destination location can be the ACS or a file server.
CPE status and performance monitoring
The ACS can monitor the status and performance of CPEs. Table 1 shows the available CPE status and performance objects for the ACS to monitor.
Table 1 CPE status and performance objects available for the ACS to monitor
Category
Objects
Remarks
Device information
Manufacturer
ManufacturerOUI
SerialNumber
HardwareVersion
SoftwareVersion
N/A
Operating status and information
DeviceStatus
UpTime
N/A
Configuration file
ConfigFile
Local configuration file stored on CPE for upgrade. The ACS can issue configuration to the CPE by transferring a configuration file to the CPE or running the configuration in CPE's RAM.
CWMP settings
ACS URL
URL address of the ACS to which the CPE initiates a CWMP connection. This object is also used for main/backup ACS switchover.
ACS username
ACS password
When the username and password of the ACS are changed, the ACS changes the ACS username and password on the CPE to the new username and password.
When a main/backup ACS switchover occurs, the main ACS also changes the ACS username and password to the backup ACS username and password.
PeriodicInformEnable
Whether to enable or disable the periodic Inform feature.
PeriodicInformInterval
Interval for periodic connection from the CPE to the ACS for configuration and software update.
PeriodicInformTime
Scheduled time for connection from the CPE to the ACS for configuration and software update.
ConnectionRequestURL (CPE URL)
N/A
ConnectionRequestUsername (CPE username)
ConnectionRequestPassword (CPE password)
CPE username and password for authentication from the ACS to the CPE.
How CWMP works
RPC methods
CWMP uses remote procedure call (RPC) methods for bidirectional communication between CPE and ACS. The RPC methods are encapsulated in HTTP or HTTPS.
Table 2 shows the primary RPC methods used in CWMP.
Table 2 RPC methods
RPC method
Get
The ACS obtains the values of parameters on the CPE.
Set
The ACS modifies the values of parameters on the CPE.
Inform
The CPE sends an Inform message to the ACS for the following purposes:
·     Initiates a connection to the ACS.
·     Reports configuration changes to the ACS.
·     Periodically updates CPE settings to the ACS.
Download
The ACS requires the CPE to download a configuration or software image file from a specific URL for software or configuration update.
Upload
The ACS requires the CPE to upload a file to a specific URL.
Reboot
The ACS reboots the CPE remotely for the CPE to complete an upgrade or recover from an error condition.
Autoconnect between ACS and CPE
The CPE automatically initiates a connection to the ACS when one of the following events occurs:
·     ACS URL change. The CPE initiates a connection request to the new ACS URL.
·     CPE startup. The CPE initiates a connection to the ACS after the startup.
·     Timeout of the periodic Inform interval. The CPE re-initiates a connection to the ACS at the Inform interval.
·     Expiration of the scheduled connection initiation time. The CPE initiates a connection to the ACS at the scheduled time.
CWMP connection establishment
Step 1 through step 5 in Figure 2 show the procedure of establishing a connection between the CPE and the ACS.
1.     After obtaining the basic ACS parameters, the CPE initiates a TCP connection to the ACS.
2.     If HTTPS is used, the CPE and the ACS initialize SSL for a secure HTTP connection.
3.     The CPE sends an Inform message in HTTPS to initiate a CWMP session.
4.     After the CPE passes authentication, the ACS returns an Inform response to establish the session.
5.     After sending all requests, the CPE sends an empty HTTP post message.
Figure 2 CWMP connection establishment
Main/backup ACS switchover
Typically, two ACSs are used in a CWMP network for consecutive monitoring on CPEs. When the main ACS needs to reboot, it points the CPE to the backup ACS. Step 6 through step 11 in Figure 3 show the procedure of a main/backup ACS switchover.
1.     Before the main ACS reboots, it queries the ACS URL set on the CPE.
2.     The CPE replies with its ACS URL setting.
3.     The main ACS sends a Set request to change the ACS URL on the CPE to the backup ACS URL.
4.     After the ACS URL is modified, the CPE sends a response.
5.     The main ACS sends an empty HTTP message to notify the CPE that it has no other requests.
6.     The CPE closes the connection, and then initiates a new connection to the backup ACS URL.
Figure 3 Main and backup ACS switchover
Restrictions and guidelines: CWMP configuration
You can configure ACS and CPE attributes from the CPE's CLI, the DHCP server, or the ACS. For an attribute, the CLI- and ACS-assigned values have higher priority than the DHCP-assigned value. The CLI- and ACS-assigned values overwrite each other, whichever is assigned later.
This document only describes configuring ACS and CPE attributes from the CLI and DHCP server. For more information about configuring and using the ACS, see ACS documentation.
CWMP tasks at a glance
To configure CWMP, perform the following tasks:
1.     Enabling CWMP from the CLI
You can also enable CWMP from a DHCP server.
2.     Configuring ACS attributes
a.     Configuring the preferred ACS attributes
b.     (Optional.) Configuring the default ACS attributes from the CLI
3.     Configuring CPE attributes
a.     Specifying an SSL client policy for HTTPS connection to ACS
This task is required when the ACS uses HTTPS for secure access.
b.     (Optional.) Configuring ACS authentication parameters
c.     (Optional.) Configuring the provision code
d.     (Optional.) Configuring the CWMP connection interface
e.     (Optional.) Configuring autoconnect parameters
f.     (Optional.) Setting the close-wait timer
g.     (Optional.) Enabling NAT traversal for the CPE
2.     Enter CWMP view.
cwmp
3.     Enable CWMP.
cwmp enable
By default, CWMP is disabled.
About ACS attributes
You can configure two sets of ACS attributes for the CPE: preferred and default.
·     The preferred ACS attributes are configurable from the CPE's CLI, the DHCP server, and ACS.
·     The default ACS attributes are configurable only from the CLI.
If the preferred ACS attributes are not configured, the CPE uses the default ACS attributes for connection establishment.
Assigning ACS attributes from the DHCP server
The DHCP server in a CWMP network assigns the following information to CPEs:
·     IP addresses for the CPEs.
·     DNS server address.
·     ACS URL and ACS login authentication information.
This section introduces how to use DHCP option 43 to assign the ACS URL and ACS login authentication username and password. For more information about DHCP and DNS, see Layer 3—IP Services Configuration Guide.
If the DHCP server is an H3C device, you can configure DHCP option 43 by using the option 43 hex 01length URL username password command.
·     length—A hexadecimal number that indicates the total length of the length, URL, username, and password arguments, including the spaces between these arguments. No space is allowed between the 01 keyword and the length value.
·     URL—ACS URL.
·     username—Username for the CPE to authenticate to the ACS.
·     password—Password for the CPE to authenticate to the ACS.
The ACS URL, username and password must use the hexadecimal format and be space separated.
The following example configures the ACS address as http://169.254.76.31:7547/acs, username as 1234, and password as 5678:
[Sysname] dhcp server ip-pool 0
[Sysname-dhcp-pool-0] option 43 hex 0127687474703A2F2F3136392E3235342E37362E33313A373534372F61637320313233342035363738
Table 3 Hexadecimal forms of the ACS attributes
Attribute
Attribute value
Hexadecimal form
Length
39 characters
27
ACS URL
The two ending digits (20) represent the space.
ACS connect username
1234
3132333420
ACS connect password
5678
35363738
Configuring the preferred ACS attributes from the CLI
2.     Enter CWMP view.
cwmp
3.     Configure the preferred ACS URL.
cwmp acs url url
By default, no preferred ACS URL has been configured.
4.     Configure the username for authentication to the preferred ACS URL.
cwmp acs username username
By default, no username has been configured for authentication to the preferred ACS URL.
5.     (Optional.) Configure the password for authentication to the preferred ACS URL.
cwmp acs password { cipher | simple } string
By default, no password has been configured for authentication to the preferred ACS URL.
2.     Enter CWMP view.
cwmp
3.     Configure the default ACS URL.
cwmp acs default url url
By default, no default ACS URL has been configured.
4.     Configure the username for authentication to the default ACS URL.
cwmp acs default username username
By default, no username has been configured for authentication to the default ACS URL.
5.     (Optional.) Configure the password for authentication to the default ACS URL.
cwmp acs default password { cipher | simple } string
By default, no password has been configured for authentication to the default ACS URL.
About CPE attributes
You can configure the following CPE attributes only from the CPE's CLI.
·     CWMP connection interface.
·     NAT traversal.
·     Maximum number of connection retries.
·     SSL client policy for HTTPS connection to ACS.
For other CPE attribute values, you can assign them to the CPE from the CPE's CLI or the ACS. The CLI- and ACS-assigned values overwrite each other, whichever is assigned later.
About specifying an SSL client policy for HTTPS connection to ACS
This task is required when the ACS uses HTTPS for secure access. CWMP uses HTTP or HTTPS for data transmission. When HTTPS is used, the ACS URL begins with https://. You must specify an SSL client policy for the CPE to authenticate the ACS for HTTPS connection establishment.
Before you perform this task, first create an SSL client policy. For more information about configuring SSL client policies, see Security Configuration Guide.
2.     Enter CWMP view.
cwmp
3.     Specify an SSL client policy.
ssl client-policy policy-name
By default, no SSL client policy is specified.
About ACS authentication parameters
To protect the CPE against unauthorized access, configure a CPE username and password for ACS authentication. When an ACS initiates a connection to the CPE, the ACS must provide the correct username and password.
2.     Enter CWMP view.
cwmp
3.     Configure the username for authentication to the CPE.
cwmp cpe username username
By default, no username has been configured for authentication to the CPE.
4.     (Optional.) Configure the password for authentication to the CPE.
cwmp cpe password { cipher | simple } string
By default, no password has been configured for authentication to the CPE.
The password setting is optional. You can specify only a username for authentication.
About the provision code
The ACS can use the provision code to identify services assigned to each CPE. For correct configuration deployment, make sure the same provision code is configured on the CPE and the ACS. For information about the support of your ACS for provision codes, see the ACS documentation.
2.     Enter CWMP view.
cwmp
3.     Configure the provision code.
cwmp cpe provision-code provision-code
The default provision code is PROVISIONINGCODE.
About CWMP connection interface configuration
The CWMP connection interface is the interface that the CPE uses to communicate with the ACS. To establish a CWMP connection, the CPE sends the IP address of this interface in the Inform messages, and the ACS replies to this IP address.
Typically, the CPE selects the CWMP connection interface automatically. If the CWMP connection interface is not the interface that connects the CPE to the ACS, the CPE fails to establish a CWMP connection with the ACS. In this case, you need to manually set the CWMP connection interface.
2.     Enter CWMP view.
cwmp
3.     Specify the interface that connects to the ACS as the CWMP connection interface.
cwmp cpe connect interface interface-type interface-number
By default, no CWMP connection interface is specified.
About autoconnect parameters
You can configure the CPE to connect to the ACS periodically, or at a scheduled time for configuration or software update.
The CPE retries a connection automatically when one of the following events occurs:
·     The CPE fails to connect to the ACS. The CPE considers a connection attempt as having failed when the close-wait timer expires. This timer starts when the CPE sends an Inform request. If the CPE fails to receive a response before the timer expires, the CPE resends the Inform request.
·     The connection is disconnected before the session on the connection is completed.
To protect system resources, limit the number of retries that the CPE can make to connect to the ACS.
Configuring the periodic Inform feature
2.     Enter CWMP view.
cwmp
3.     Enable the periodic Inform feature.
cwmp cpe inform interval enable
By default, this function is disabled.
4.     Set the Inform interval.
cwmp cpe inform interval interval
By default, the CPE sends an Inform message to start a session every 600 seconds.
Scheduling a connection initiation
2.     Enter CWMP view.
cwmp
3.     Schedule a connection initiation.
cwmp cpe inform time time
By default, no connection initiation has been scheduled.
Setting the maximum number of connection retries
2.     Enter CWMP view.
cwmp
3.     Set the maximum number of connection retries.
cwmp cpe connect retry retries
By default, the CPE retries a failed connection until the connection is established.
About the close-wait timer
The close-wait timer specifies the following:
·     The maximum amount of time the CPE waits for the response to a session request. The CPE determines that its session attempt has failed when the timer expires.
·     The amount of time the connection to the ACS can be idle before it is terminated. The CPE terminates the connection to the ACS if no traffic is sent or received before the timer expires.
2.     Enter CWMP view.
cwmp
3.     Set the close-wait timer.
cwmp cpe wait timeout seconds
By default, the close-wait timer is 30 seconds.
About NAT traversal
For the connection request initiated from the ACS to reach the CPE, you must enable NAT traversal on the CPE when a NAT gateway resides between the CPE and the ACS.
The NAT traversal feature complies with RFC 3489 Simple Traversal of UDP Through NATs (STUN). The feature enables the CPE to discover the NAT gateway, and obtain an open NAT binding (a public IP address and port binding) through which the ACS can send unsolicited packets. The CPE sends the binding to the ACS when it initiates a connection to the ACS. For the connection requests sent by the ACS at any time to reach the CPE, the CPE maintains the open NAT binding. For more information about NAT, see Layer 3—IP Services Configuration Guide.
2.     Enter CWMP view.
cwmp
3.     Enable NAT traversal.
cwmp cpe stun enable
By default, NAT traversal is disabled on the CPE.
Display and maintenance commands for CWMP
Display CWMP configuration.
display cwmp configuration
Display the current status of CWMP.
display cwmp status
CWMP configuration examples
Example: Configuring CWMP
As shown in Figure 4, use H3C IMC BIMS as the ACS to bulk-configure the devices (CPEs), and assign ACS attributes to the CPEs from the DHCP server.
The configuration files for the CPEs in equipment rooms A and B are configure1.cfg and configure2.cfg, respectively.
Figure 4 Network diagram
Table 4 shows the ACS attributes for the CPEs to connect to the ACS.
Table 4 ACS attributes
Item
Setting
Preferred ACS URL
http://10.185.10.41:9090
ACS username
admin
ACS password
12345
Table 5 lists serial numbers of the CPEs.
Table 5 CPE list
Room
Device
Serial number
A
CPE 1
210231A95YH10C000045
CPE 2
210235AOLNH12000010
CPE 3
210235AOLNH12000015
B
CPE 4
210235AOLNH12000017
CPE 5
210235AOLNH12000020
CPE 6
210235AOLNH12000022
Configuring the ACS
Figures in this section are for illustration only.
To configure the ACS:
1.     Log in to the ACS:
a.     Launch a Web browser on the ACS configuration terminal.
b.     In the address bar of the Web browser, enter the ACS URL and port number. This example uses http://10.185.10.41:8080/imc.
c.     On the login page, enter the ACS login username and password, and then click Login.
2.     Create a CPE group for each equipment room:
a.     Select Service > BIMS > CPE Group from the top navigation bar.
The CPE Group page appears.
Figure 5 CPE Group page
b.     Click Add.
c.     Enter a username, and then click OK.
Figure 6 Adding a CPE group
d.     Repeat the previous two steps to create a CPE group for CPEs in Room B.
3.     Add CPEs to the CPE group for each equipment room:
a.     Select Service > BIMS > Resource Management > Add CPE from the top navigation bar.
b.     On the Add CPE page, configure the following parameters:
-     Authentication Type—Select ACS UserName.
-     CPE Name—Enter a CPE name.
-     ACS Username—Enter admin.
-     ACS Password Generated—Select Manual Input.
-     ACS Password—Enter a password for ACS authentication.
-     ACS Confirm Password—Re-enter the password.
-     CPE Model—Select the CPE model.
-     CPE Group—Select the CPE group.
Figure 7 Adding a CPE
c.     Click OK.
d.     Verify that the CPE has been added successfully from the All CPEs page.
Figure 8 Viewing CPEs
e.     Repeat the previous steps to add CPE 2 and CPE 3 to the CPE group for Room A, and add CPEs in Room B to the CPE group for Room B.
4.     Configure a configuration template for each equipment room:
a.     Select Service > BIMS > Configuration Management > Configuration Templates from the top navigation bar.
Figure 9 Configuration Templates page
b.     Click Import.
c.     Select a source configuration file, select Configuration Segment as the template type, and then click OK.
The created configuration template will be displayed in the Configuration Template list after a successful file import.
IMPORTANT
IMPORTANT:
If the first command in the configuration template file is system-view, make sure no characters exist in front of the command.
Figure 10 Importing a configuration template
Figure 11 Configuration Template list
d.     Repeat the previous steps to configure a configuration template for Room B.
5.     Add software library entries:
a.     Select Service > BIMS > Configuration Management > Software Library from the top navigation bar.
Figure 12 Software Library page
b.     Click Import.
c.     Select a source file, and then click OK.
Figure 13 Importing CPE software
d.     Repeat the previous steps to add software library entries for CPEs of different models.
6.     Create an auto-deployment task for each equipment room:
a.     Select Service > BIMS > Configuration Management > Deployment Guide from the top navigation bar.
Figure 14 Deployment Guide
b.     Click By CPE Model from the Auto Deployment Configuration field.
c.     Select a configuration template, select Startup Configuration from the File Type to be Deployed list, and click Select Model to select CPEs in Room A. Then, click OK.
You can search for CPEs by CPE group.
Figure 15 Auto deployment configuration
d.     Click OK on the Auto Deploy Configuration page.
Figure 16 Operation result
e.     Repeat the previous steps to add a deployment task for CPEs in Room B.
Configuring the DHCP server
In this example, an H3C device is operating as the DHCP server.
1.     Configure an IP address pool to assign IP addresses and DNS server address to the CPEs. This example uses subnet 10.185.10.0/24 for IP address assignment.
# Enable DHCP.
<DHCP_server> system-view
[DHCP_server] dhcp enable
# Enable DHCP server on VLAN-interface 1.
[DHCP_server] interface vlan-interface 1
[DHCP_server-Vlan-interface1] dhcp select server
[DHCP_server-Vlan-interface1] quit
# Exclude the DNS server address 10.185.10.60 and the ACS IP address 10.185.10.41 from dynamic allocation.
[DHCP_server] dhcp server forbidden-ip 10.185.10.41
[DHCP_server] dhcp server forbidden-ip 10.185.10.60
# Create DHCP address pool 0.
[DHCP_server] dhcp server ip-pool 0
# Assign subnet 10.185.10.0/24 to the address pool, and specify the DNS server address 10.185.10.60 in the address pool.
[DHCP_server-dhcp-pool-0] network 10.185.10.0 mask 255.255.255.0
[DHCP_server-dhcp-pool-0] dns-list 10.185.10.60
2.     Configure DHCP Option 43 to contain the ACS URL, username, and password in hexadecimal format.
[DHCP_server-dhcp-pool-0] option 43 hex 013B687474703A2F2F6163732E64617461626173653A393039302F616373207669636B79203132333435
Configuring the DNS server
Map http://acs.database:9090 to http://10.185.1.41:9090 on the DNS server. For more information about DNS configuration, see DNS server documentation.
Connecting the CPEs to the network
# Connect CPE 1 to the network, and then power on the CPE. (Details not shown.)
# Log in to CPE 1 and configure VLAN-interface 2 to use DHCP for IP address acquisition, and assign GigabitEthernet 1/0/1 to VLAN-interface 2. At startup, the CPE obtains the IP address and ACS information from the DHCP server to initiate a connection to the ACS. After the connection is established, the CPE interacts with the ACS to complete autoconfiguration.
<CPE1> system-view
[CPE1] vlan 2
[CPE1-vlan2] quit
[CPE1] interface gigabitethernet 1/0/1
[CPE1-GigabitEthernet1/0/1] port access vlan 2
[CPE1-GigabitEthernet1/0/1] quit
[CPE1] interface vlan-interface 2
[CPE1-Vlan-interface2] ip address dhcp-alloc
# Repeat the previous steps to configure the other CPEs.
# Execute the display current-configuration command to verify that the running configurations on CPEs are the same as the configurations issued by the ACS.