11-Network Management and Monitoring Configuration Guide
HomeSupportSwitchesS12500R SeriesConfigure & DeployConfiguration GuidesH3C S12500R Switch Router Series Configuration Guides(R36xx)-6W10111-Network Management and Monitoring Configuration Guide
04-PTP configuration
04-PTP configuration 386.35 KB
Configuring PTP·· 1
About PTP· 1
Basic concepts· 1
Grandmaster clock selection and master-member/subordinate relationship establishment 3
Synchronization mechanism·· 3
Protocols and standards· 5
Restrictions: Hardware compatibility with PTP· 5
Restrictions and guidelines: PTP configuration· 5
PTP tasks at a glance· 6
Configuring PTP (IEEE 1588 version 2) 6
Configuring PTP (IEEE 802.1AS) 7
Specifying PTP for obtaining the time· 7
Specifying a PTP profile· 7
Configuring clock nodes· 8
Specifying a clock node type· 8
Configuring an OC to operate only as a member clock· 8
Specifying a PTP domain· 9
Enabling PTP on a port 9
Configuring PTP ports· 9
Configuring the role of a PTP port 9
Configuring the mode for carrying timestamps· 10
Specifying a delay measurement mechanism·· 10
Configuring one of the ports on a TC+OC clock as an OC-type port 11
Configuring PTP message transmission and receiving· 12
Setting the interval for sending announce messages and the timeout multiplier for receiving announce messages  12
Setting the interval for sending Pdelay_Req messages· 12
Setting the interval for sending Sync messages· 12
Setting the minimum interval for sending Delay_Req messages· 13
Configuring parameters for PTP messages· 13
Specifying UDP encapsulation of PTP messages· 13
Configuring a source IP address for multicast PTP messages transmitted over IPv4 UDP· 14
Configuring a destination IP address for unicast PTP messages transmitted over IPv4 UDP· 14
Configuring the destination MAC address for PTP messages· 15
Setting a DSCP value for PTP messages transmitted over IPv4 UDP· 16
Specifying a VLAN tag for PTP messages· 16
Disabling PTP path tracing· 16
Specifying the maximum number of removed steps (clock nodes) from the GM to the device· 17
Enabling the device to notify the downstream nodes of its time synchronization state· 17
Adjusting and correcting clock synchronization· 18
Setting the delay correction value· 18
Setting the cumulative offset between the UTC and TAI 18
Setting the correction date of the UTC· 18
Setting clock source parameters· 19
Configuring clock priorities· 19
Configuring a priority for a clock (IEEE 1588 version 2 and IEEE 802.1AS) 19
Configuring PTP logging· 20
Display and maintenance commands for PTP· 21
PTP configuration examples· 21
Example: Configuring PTP (IEEE 1588 version 2, IEEE 802.3/Ethernet encapsulation, multicast transmission) 21
Example: Configuring PTP (IEEE 1588 version 2, IPv4 UDP encapsulation, multicast transmission) 24
Example: Configuring PTP (IEEE 1588 version 2, IPv4 UDP encapsulation, unicast transmission) 28
Example: Configuring PTP (IEEE 802.1AS, IEEE 802.3/Ethernet encapsulation, multicast transmission) 31
Configuring PTP
About PTP
Precision Time Protocol (PTP) provides time synchronization among devices with submicrosecond accuracy. It provides also precise frequency synchronization.
Basic concepts
PTP profile
PTP profiles (PTP standards) include:
·     IEEE 1588 version 2—1588v2 defines high-accuracy clock synchronization mechanisms. It can be customized, enhanced, or tailored as needed. 1588v2 is the latest version.
·     IEEE 802.1AS—802.1AS is introduced based on IEEE 1588. It specifies a profile for use of IEEE 1588-2008 for time synchronization over a virtual bridged local area network (as defined by IEEE 802.1Q). 802.1AS supports point-to-point full-duplex Ethernet, IEEE 802.11, and IEEE 802.3 EPON links.
PTP domain
A PTP domain refers to a network that is enabled with PTP. A PTP domain has only one reference clock called "grandmaster clock (GM)." All devices in the domain synchronize to the clock.
Clock nodes and PTP ports (IEEE 1588 version 2 and IEEE 802.1AS)
In a PTP domain, a node is called a clock node and the ports running PTP are called PTP ports. IEEE 1588 version 2 and IEEE 802.1AS define the following types of basic clock nodes:
·     Ordinary Clock (OC)—A clock node with a single PTP port in a PTP domain for time synchronization. It synchronizes time from its upstream clock node through the port. If an OC operates as the clock source, it sends synchronization time through a single PTP port to its downstream clock nodes.
·     Boundary Clock (BC)—A clock node with more than one PTP port in a PTP domain for time synchronization. A BC uses one of the ports to synchronize time from its upstream clock node. It uses the other ports to synchronize time to the relevant downstream clock nodes. If a BC operates as the clock source, such as BC 1 in Figure 1, it synchronizes time through multiple PTP ports to its downstream clock nodes.
·     Transparent Clock (TC)—A TC clock node does not keep time consistency with other clock nodes. A TC has multiple PTP ports. It forwards PTP messages among these ports and performs delay corrections for the messages, instead of performing time synchronization. TCs include the following types:
¡     End-to-End Transparent Clock (E2ETC)—Forwards non-P2P PTP messages in the network and calculates the delay of the entire link.
¡     Peer-to-Peer Transparent Clock (P2PTC)—Forwards only Sync, Follow_Up, and Announce messages, terminates other PTP messages, and calculates the delay of each link segment.
Figure 1 shows the positions of these basic clock nodes in a PTP domain.
Figure 1 Clock nodes and PTP ports in a PTP domain (IEEE 1588 version 2 and IEEE 802.1AS)
In addition to these basic types of clock nodes, PTP introduces hybrid clock nodes. For example, a TC+OC has multiple PTP ports in a PTP domain. One port is the OC type, and the others are the TC type. A TC+OC forwards PTP messages and performs delay corrections through TC-type ports. In addition, it synchronizes time through its OC-type port. TC+OCs include these types: E2ETC+OC and P2PTC+OC.
Technical standard
A PTP profile uses the parameters including time accuracy, time class, time source, and clock offset (log variance) to describe PTP clock source signals. Users can customize and supplement a PTP profile based on the network conditions to develop their own PTP technical standard.
Three PTP technical standards are available: the default technical standard, OAM technical standard, and Unicom technical standard. The default parameter values, the elected clock source, and PTP message processing vary by technical standard.
Master-member/subordinate relationship
The master-member/subordinate relationship is automatically determined based on the Best Master Clock (BMC) algorithm. You can also manually specify a role for the clock nodes.
The master-member/subordinate relationship is defined as follows:
·     Master/Member node—A master node sends a synchronization message, and a member node receives the synchronization message.
·     Master/Member clock—The clock on a master node is a master clock (parent clock). The clock on a member node is a member clock.
·     Master/Subordinate port—A master port sends a synchronization message, and a subordinate port receives the synchronization message. The master and subordinate ports can be on a BC or an OC.
A port that neither receives nor sends synchronization messages is a passive port.
Clock source type
A clock node supports the following clock sources:
·     Local clock—38.88 MHz clock signals generated by a crystal oscillator inside the clock monitoring module.
·     External clock source—Clock signals generated by an external clock device. The signals are received and sent by a 1PPS/ToD port on the device. It is also called a ToD clock source.
Grandmaster clock
As shown in Figure 1, the grandmaster clock (GM) is the ultimate source of time for clock synchronization in a PTP domain. It is elected automatically by the clock nodes in the PTP domain. The clock nodes exchange PTP messages and elect the GM by comparing the clock priority, time class, and time accuracy carried in the PTP messages.
You can also specify a GM manually.
A GM can be manually specified. It can also be automatically elected through the BMC algorithm as follows:
1.     The clock nodes in a PTP domain exchange announce messages and elect a GM by using the following rules in descending order of precedence:
a.     Clock node with higher priority 1.
b.     Clock node with higher time class.
c.     Clock node with higher time accuracy.
d.     Clock node with higher priority 2.
e.     Clock node with a smaller port ID (containing clock number and port number).
The master nodes, member nodes, master ports, and subordinate ports are determined during the process. Then a spanning tree with the GM as the root is generated for the PTP domain.
2.     The master node periodically sends announce messages to the member nodes. If the member nodes do not receive announce messages from the master node, they determine that the master node is invalid, and they start to elect another GM.
After master-member relationships are established between the clock nodes, the master and member clock nodes exchange PTP messages and record the message transmit and receive time. Based on the timestamps, each member clock calculates the path delay between them and the master clock and adjusts their time accordingly for time synchronization with the master clock.
PTP defines two path delay measurement mechanisms: Request_Response_ and Peer Delay, both of which are based on network symmetry.
Request_Response
The Request_Response mechanism measures the average path delay between the master and member clock nodes by using the Sync, Delay_Req, Delay_Resp, and Follow_Up messages as shown in Figure 2. A TC between master and member clock nodes does not calculate the path delay. It forwards PTP messages and notifies the member clock of the PTP message residence time on it.
This mechanism can be implemented in one of the following two modes:
·     Two-step mode—t1 is carried in the Follow_Up message, as shown in Figure 2.
·     Single-step mode—t1 is carried in the Sync message, and no Follow_Up message is sent.
Figure 2 shows the Request_Response mechanism in two-step mode.
1.     The master clock sends a Sync message to the member clock, and records the sending time t1. Upon receiving the message, the member clock records the receiving time t2.
2.     After sending the Sync message, the master clock immediately sends a Follow_Up message that carries time t1.
3.     The member clock sends a Delay_Req message to the master clock, and records the sending time t3. Upon receiving the message, the master clock records the receiving time t4.
4.     The master clock returns a Delay_Resp message that carries time t4.
After this procedure, the member clock obtains all four timestamps and can make the following calculations:
·     Round-trip delay between the master and member clocks: (t2 t1) + (t4 t3)
·     One-way delay between the master and member clocks: [(t2 – t1) + (t4 – t3)] / 2
·     Offset between the member and master clocks: (t2 – t1) – [(t2 – t1) + (t4 – t3)] / 2 or [(t2 – t1) – (t4 – t3)] / 2
Figure 2 Request_Response mechanism (two-step node)
Peer Delay
The Peer Delay mechanism measures the average path delay between two clock nodes by using Pdelay messages. TCs that exist between master and member clock nodes will divide the synchronization path into multiple links. They calculate the link delays and notify the member clock of the link delays and PTP message residence time on them.
·     Two-step mode
As shown in Figure 3, Pdelay messages include Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages. t2 is carried in the Pdelay_Resp message, and t3 is carried in the Pdelay_Resp_Follow_Up message.
·     Single-step mode
Pdelay messages include Pdelay_Req and Pdelay_Resp messages. t3 – t2 is carried in the Pdelay_Resp, and no Pdelay_Resp_Follow_Up message is sent.
The two clock nodes (BC, TC or OC) using this mechanism will send Pdelay messages to each other, and calculate the one-way link delay between them independently. The message interaction process and delay calculation method are identical on the two nodes. Figure 3 uses Clock node B as an example to describe the Peer Delay mechanism.
1.     Clock node B sends a Pdelay_Req message to Clock node A, and records the sending time t1. Upon receiving the message, Clock node A records the receiving time t2.
2.     Clock node A sends a Pdelay_Req message that carries t2 to Clock node B, and records the sending time t3. Upon receiving the message, Clock node B records the receiving time t4.
3.     Clock node A immediately sends a Pdelay_Resp_Follow_Up message carrying t3 to Clock node B after sending the Pdelay_Req message.
After this procedure, Clock node B obtains all four timestamps and can make the following calculations:
·     Round-trip delay between Clock node A and Clock node B: (t2 – t1) + (t4 – t3)
·     One-way delay between Clock node A and Clock node B: [(t2 – t1) + (t4 – t3)] / 2 = [(t3 – t2) + (t4 – t1)] / 2
·     Time offset between the member clock and the master clock: Sync message receiving time on the member clock Sync message sending time on the master clock – Total one-way delays on all links – Total PTP message residence time on all TCs.
Figure 3 Peer Delay mechanism (two-step mode)
·     IEEE 1588-2008, IEEE Standard for a Precision Clock Synchronization Protocol for Networked Measurement and Control Systems
·     IEEE 802.1AS, Timing and Synchronization for Time-Sensitive Applications in Bridged Local Area Networks
Only the HBR (except the LSXM1CGQ36HBR1) and HFR (except the LSXM1CGQ36HFR1) cards that operate together with the LSXM1SUP04TR1 or LSXM1SUPER1 MPU support PTP.
The feature is supported only when the system operates in bridgee mode. You can use the display system-working-mode command to view the system operating mode. For more information about the system operating mode, see device management configuration in Fundamentals Configuration Guide.
Before configuring PTP, determine the PTP standard and define the scope of the PTP domain and the role of every clock node.
When the PTP profile is IEEE 1588 version 2, specify the BC or OC clock node type for the devices. A TC clock node is mainly used for forwarding PTP messages. When receiving a PTP message, a TC multicasts the message from all its PTP interfaces except the inbound interface of the PTP message. To deploy a TC, plan the TC location and number and location of PTP interfaces on the TC manually to prevent PTP forwarding loops.
1.     Specifying PTP for obtaining the time
2.     Specifying a PTP profile
Specify the IEEE 1588 version 2 PTP profile.
3.     Configuring clock nodes
¡     Specifying a clock node type
¡     (Optional.) Configuring an OC to operate only as a member clock
4.     (Optional.) Specifying a PTP domain
5.     Enabling PTP on a port
6.     Configuring PTP ports
¡     (Optional.) Configuring the role of a PTP port
¡     Configuring the mode for carrying timestamps
¡     Specifying a delay measurement mechanism
¡     Configuring one of the ports on a TC+OC clock as an OC-type port
7.     (Optional.) Configuring PTP message transmission and receiving
¡     Setting the interval for sending announce messages and the timeout multiplier for receiving announce messages
¡     Setting the interval for sending Pdelay_Req messages
¡     Setting the interval for sending Sync messages
¡     Setting the minimum interval for sending Delay_Req messages
8.     (Optional.) Configuring parameters for PTP messages
¡     Specifying UDP encapsulation of PTP messages
¡     Configuring a source IP address for multicast PTP messages transmitted
¡     Configuring a destination IP address for unicast PTP messages transmitted
¡     Configuring the destination MAC address for PTP messages
¡     Setting a DSCP value for PTP messages transmitted
¡     Specifying a VLAN tag for PTP messages
9.     (Optional.) Disabling PTP path tracing
10.     (Optional.) Adjusting and correcting clock synchronization
¡     Setting the delay correction value
¡     Setting the cumulative offset between the UTC and TAI
¡     Setting the correction date of the UTC
11.     (Optional.) Setting clock source parameters
12.     (Optional.) Configuring clock priorities
¡     Configuring a priority for a clock (IEEE 1588 version 2 and IEEE 802.1AS)
13.     (Optional.) Configuring PTP logging
Specify the IEEE 802.1AS PTP profile.
8.     (Optional.) Specifying a VLAN tag for PTP messages
13.     Configuring a priority for a clock (IEEE 1588 version 2 and IEEE 802.1AS)
2.     Specify PTP for obtaining the time.
clock protocol ptp
By default, the device uses NTP to synchronize the system time.
For more information about the clock protocol command, see device management commands in Fundamentals Command Reference.
You must specify a PTP profile before configuring PTP settings. Changing the PTP profile clears all settings under the profile.
2.     Specify a PTP profile.
ptp profile { 1588v2 | 8021as }
By default, no PTP profile is specified for the device.
You can specify only one clock node type for the device. The clock node types include OC, BC, E2ETC, P2PTC, E2ETC+OC, and P2PTC+OC.
Before you specify a clock node type, specify a PTP profile. When the PTP profile is IEEE 802.1AS, you cannot specify the E2ETC or E2ETC+OC clock node type.
2.     Specify a clock node type.
ptp mode { bc | e2etc | e2etc-oc | oc | p2ptc | p2ptc-oc }
By default, no clock node type is specified.
An OC can operate either as a master clock to send synchronization messages or as a member clock to receive synchronization messages. This task allows you to configure an OC to operate only as a member clock.
If an OC is operating only as a member clock, you can use the ptp force-state command to configure its PTP port as a master port or passive port.
This task is applicable only to OCs.
2.     Configure the OC to operate only as a member clock.
ptp slave-only
By default, an OC operates as a master or member clock.
Within a PTP domain, all devices follow the same rules to communicate with each other. Devices in different PTP domains cannot exchange PTP messages.
2.     Specify a PTP domain for the device.
ptp domain value
When the PTP profile is IEEE 1588 version 2 or IEEE 802.1AS, the device belongs to PTP domain 0 by default.
A port enabled with PTP becomes a PTP port.
You can enable PTP on only one port on an OC, T-TSC, or T-TSC-P clock node.
To enable PTP on a Layer 3 Ethernet interface that has been assigned to a VPN instance, you must specify this VPN instance in the ptp source ip-address vpn-instance vpn-instance-name command if PTP messages are to be transmitted in multicast mode over IPv4 UDP.
2.     Enter Layer 2 Ethernet interface view or Layer 3 Ethernet interface view.
3.     Enable PTP on the port.
ptp enable
By default, PTP is disabled on a port.
You can configure the master, passive, or slave role for a PTP port.
For an OC that operates in slave-only mode, you can perform this task to change its PTP port role to master or slave.
By default, the PTP port roles are automatically negotiated based on the BMC algorithm. If you use the ptp force-state command to change the role of one PTP port, all the other PTP ports in the PTP domain stop working. For these PTP ports to function, you must specify roles for each of them by using the ptp force-state command. As a best practice, enable automatic negotiation of PTP port roles based on the BMC algorithm.
You can configure only one subordinate port on a device.
After you change the role of a PTP port, you must execute the ptp active force-state command to activate the port role configuration.
3.     Configure the role of the PTP port.
ptp force-state { master | passive | slave }
By default, the PTP port role is automatically calculated through BMC.
4.     Return to system view.
5.     Activate the port role configuration.
By default, the port role configuration is not activated.
Timestamps are carried in two-step mode. The Sync and Pdelay_Resp message sending timestamps are not carried by the message itself but a subsequent message.
IEEE 802.1AS supports only the two-step mode.
3.     Configure the mode for carrying timestamps.
ptp clock-step { one-step | two-step }
By default, two-step mode is used for carrying  timestamps.
PTP defines two transmission delay measurement mechanisms: Request_Response and Peer Delay. For correct communication, ports on the same link must share the same delay measurement mechanism.
You can configure this task only for BCs and OCs.
The delay measurement mechanism is Request_Response for E2ETCs and E2ETC+OCs and Peer Delay for P2PTCs and P2PTC+OCs. You cannot change the delay measurement mechanism for these clock nodes.
The IEEE 802.1AS PTP profile supports only the peer delay measurement mechanism. This task is not supported under the IEEE 802.1AS PTP profile.
3.     Specify a delay measurement mechanism.
ptp delay-mechanism { e2e | p2p }
The default delay measurement mechanism varies by PTP profile:
¡     IEEE 1588 version 2—Request_Response mechanism.
¡     IEEE 802.1AS—Peer Delay mechanism
¡     The e2e keyword indicates the Request_Response mechanism, and the p2p keyword indicates the Peer Delay mechanism.
All ports on a TC+OC (E2ETC+OC or P2PTC+OC) are TC-type ports by default. This feature allows you to configure one of the ports on a TC+OC clock as an OC-type port.
This task is applicable only to E2ETC+OCs and P2PTC+OCs.
For time synchronization accuracy, the OC-type port on an E2ETC+OC or P2PTC+OC must be specified as the master port.
3.     Configure the port type as OC.
ptp port-mode oc
By default, the port type for all ports on a TC+OC is TC.
A master node sends announce messages to the member nodes at the specified interval. If a member node does not receive any announce message from the master node after the timeout expires, it determines that the master node is invalid. The timeout = timeout multiplier × interval at which the master node sends announce messages.
3.     Set the interval for sending announce messages.
ptp announce-interval interval
The default settings of the command vary by PTP profile:
¡     IEEE 1588 version 2—The interval argument value is 1 and the interval for sending announce messages is 2 (21) seconds.
¡     IEEE 802.1AS—The interval argument value is 0 and the interval for sending announce messages is 1 (20)second.
4.     Set the number of intervals before a timeout occurs.
ptp announce-timeout multiple-value
By default, a timeout occurs when three intervals are reached.
3.     Set the interval for sending Pdelay_Req messages.
ptp pdelay-req-interval interval
By default, the interval argument value is 0 and the interval for sending peer delay request messages is 1 (20) second.
A master node sends Sync messages to the member nodes at intervals set on its interfaces.
3.     Set the interval for sending Sync messages.
ptp syn-interval interval
¡     IEEE 1588 version 2—The interval argument value is 0 and the interval for sending Sync messages is 1 (20) second.
¡     IEEE 802.1AS—The interval argument value is –3 and the interval for sending Sync messages is 1/8 (2-3) seconds.
When receiving a Sync or Follow_Up message, an interface can send Delay_Req messages only when the minimum interval is reached.
This setting is not supported when the PTP protocol is IEEE 802.1AS.
In PTP multicast transport mode, this setting takes effect only when configured on the master clock. The master clock sends the value to a member clock through PTP messages to control the interval for the member clock to send Delay_Req messages. To view the value on a member clock, execute the display ptp interface command on the member clock.
In PTP unicast transport mode, this setting takes effect when configured on member clocks. It does not take effect when configured on the master clock.
3.     Set the minimum interval for sending Delay_Req messages.
ptp min-delayreq-interval interval
The default setting varies by PTP profile.
¡     IEEE 1588 version 2—The value of the interval argument is 0 and the minimum interval for sending delay request messages is 1 (20) second.
PTP messages can be encapsulated in IEEE 802.3/Ethernet packets or UDP packets.
The IEEE 802.1AS PTP profile supports only IEEE 802.3/Ethernet encapsulation of PTP messages and does not support this task.
3.     Specify UDP encapsulation of PTP messages.
ptp transport-protocol udp
By default, IEEE 802.3/Ethernet encapsulation is used for PTP messages.
To transport multicast PTP messages over IPv4 UDP, you must configure a source IP address for the messages.
If a source IP address for multicast PTP messages transmitted over IPv4 UDP and a destination address for unicast PTP messages transmitted over IPv4 UDP are both configured, the system unicasts the messages.
This task is not available under the IEEE 802.1AS PTP profile.
2.     Configure a source IP address for multicast PTP messages transmitted over IPv4 UDP.
ptp source ip-address [ vpn-instance vpn-instance-name ]
By default, no source IP address is configured for multicast PTP messages transmitted over IPv4 UDP.
UDP-encapsulated PTP messages can be transmitted in unicast or multicast.
To transmit a UDP-encapsulated message in unicast, you must configure a destination IP address for the message. The multicast destination IP address for UDP-encapsulated messages is 224.0.1.129 in Request_Response measurement mechanism and 224.0.0.107 in Peer Delay measurement mechanism.
Configure an IP address for the current interface, and make sure the interface and the peer PTP interface can reach each other.
2.     Enter Layer 3 Ethernet interface view.
3.     Configure a destination IP address for unicast PTP messages transmitted over IPv4 UDP.
ptp unicast-destination ip-address
By default, no destination IP address is configured for unicast PTP messages transmitted over IPv4 UDP.
IEEE 802.3/Ethernet-encapsulated PTP messages can be sent through multicast or unicast. The destination MAC address for PTP messages can be as follows:
·     Any unicast MAC address in unicast mode.
·     In multicast mode:
¡     0180-C200-000E or 011B-1900-0000 for non-Pdelay messages, including delay_Req, delay_Resp, delay_Resp_Follow_Up, Announce, Sync, and FollowUp messages.
¡     0180-C200-000E for Pdelay messages, including Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages.
You must specify a PTP profile and a PTP mode before configuring this task.
This command is not available for the IEEE 802.1AS PTP profile.
This feature takes effect only when PTP messages are encapsulated in IEEE 802.3/Ethernet packets.
3.     Configure the destination MAC address for PTP messages.
ptp destination-mac mac-address
By default, the destination MAC address for non-Pdelay messages is 011B-1900-0000 and the destination MAC address for Pdelay messages is 0180-C200-000E.
The DSCP value determines the sending precedence of PTP messages transmitted over IPv4 UDP.
3.     Set a DSCP value for PTP messages transmitted over IPv4 UDP.
ptp dscp dscp
By default, the DSCP value is 56.
Perform this task to configure the VLAN ID and the 802.1p precedence in the VLAN tag carried by PTP messages.
2.     Enter Layer 2 Ethernet interface view.
3.     Specify a VLAN tag for PTP messages.
ptp vlan vlan-id [ dot1p dot1p-value ]
By default, PTP messages do not have a VLAN tag.
PTP path tracing traces the clock nodes that the clock signals traverse from the GM to the device. The system can obtain complete path tracing information only when all clock nodes on the path are enabled with PTP path tracing. If a device on the path does not support PTP path tracing, disable this feature to prevent PTP communication issues.
2.     Disable PTP path tracing.
ptp path-trace disable
By default, PTP path tracing is enabled.
If the number of removed steps from the GM to the device on the PTP synchronization path is too large, the time synchronization accuracy will decrease. After you specify the maximum number of removed steps from the GM to the device, the device cannot synchronize time through PTP if the number of the removed steps exceeds the maximum value.
Software version and feature compatibility
This task is supported only in R3608 and later.
2.     Specify the maximum number of removed steps from the GM to the device.
ptp max-steps-removed step-removed-value
By default, the maximum number of removed steps from the GM to the device is 255.
The task enables the device to notify its downstream nodes of its time synchronization state.
By default, the device transfers only the locked and unlocked status of the upstream node to the downstream nodes, and does not transfer its locked or unlocked status to the downstream nodes.
After this task is configured, the device notifies the downstream nodes of its locked and unlocked status through the synchronizationUncertain flag in the announce messages. The downstream nodes do not synchronize to the device when they receive information that the device time is unlocked and synchronize to the device when they receive information that the device time is locked.
This task is available only for for the IEEE 1588 version 2 PTP profiles.
2.     Enable the device to notify the downstream nodes of its time synchronization state.
ptp sync-uncertain enable
By default, the device does not notify the downstream nodes of its time synchronization state.
PTP performs time synchronization based on the assumption that the delays in sending and receiving messages are the same. However, this is not practical. If you know the offset between the delays in sending and receiving messages, you can set the delay correction value for more accurate time synchronization.
3.     Enter Layer 3 Ethernet interface view.
4.     Set a delay correction value.
ptp asymmetry-correction { minus | plus } value
The default is 0 nanoseconds. Delay correction is not performed.
An offset exists between Coordinated Universal Time (UTC) and International Atomic Time (TAI). The device displays the UTC time. However, PTP uses TAI for time synchronization. For the device to synchronize correct time to other clock nodes in the PTP domain when its local clock is selected as the GM, configure this task to correct the offset between UTC and TAI.
2.     Set the cumulative offset between the UTC and TAI.
ptp utc offset utc-offset
The default is 0 seconds.
This task allows you to adjust the UTC at the last minute (23:59) of the specified date.
If you configure the setting multiple times, the most recent configuration takes effect.
This configuration takes effect only on the GM.
2.     Set the correction date of the UTC.
ptp utc { leap59-date | leap61-date } date
By default, the correction date of the UTC is not configured.
The clock's time class is an inherent attribute of the device. As a best practice, keep and do not change the default time class of a local clock source.
2.     Set clock source parameters. Choose one option as needed:
¡     ptp clock-source local { accuracy acc-value | class class-value | time-source ts-value }
¡     ptp clock-source { tod0 | tod1 } { accuracy acc-value | class class-value | time-source ts-value | grandmaster-clockid clock-id | offsetscaled-logvariance value }
Only the LSXM1SUPER1 card supports the ToD clock source parameters.
The default settings for clock source parameters vary by PTP profile and PTP technical standard.
¡     The clock ID of a GM clock is 000000-0000-000000. Set it manually.
¡     IEEE 1588 version 2 PTP profile
-     Local clock source—The accuracy value is 32, the time class value is 248, the offset (log variance) is 65535, and the time source value is 160. The offset (log variance) value is not configurable.
-     ToD clock source—The accuracy value is 32, the time class value is 6, the offset (log variance) is 65535, and the time source value is 32.
¡     IEEE 802.1AS PTP profile
-     Local clock source—The accuracy value is 32, the time class value is 248, the offset (log variance) is 16640, and the time source value is 160.
Priorities for clocks are used to elect the GM. The smaller the priority value, the higher the priority.
2.     Configure the priority for a clock .
ptp priority clock-source local { priority1 priority1 | priority2 priority2 }
When the PTP profile is IEEE 1588 version 2, the default value for both priority 1 and priority 2 is 128.
When the PTP profile is IEEE 802.1AS, the default value is 246 for priority 1 and 248 for priority 2.
PTP logs help monitor the clock source status. The following PTP logs are available:
·     PTP log that indicates a lower time class
Each PTP clock source has a class value. For a ToD clock source, you can set its class value by using the ptp clock-source command. The higher the value, the lower the class. When the class value of the clock source crosses the class threshold, the system outputs a log for notification.
·     PTP log that indicates a higher time offset between the external reference clock and the PTP clock
If the device uses an external reference clock, it periodically calculates the time offset between the external reference clock and the PTP clock. When the offset exceeds the threshold, the device outputs a log for notification
·     PTP logs that indicate a higher time-offset-sum peak-to-peak value
The PTP module calculates the time-offset-sum peak-to-peak value at specific intervals and compares the value with the threshold configured by this command. If the value is larger than the threshold, the system outputs a log for notification.
Only the IEEE 1588 version 2 PTP profile supports this task.
Only the LSXM1SUPER1 card supports the PTP time locking and unlocking thresholds.
2.     Configure the class threshold for the clock source.
ptp alarm-threshold clock-source-class class-value
By default, the class threshold for the clock source is 6.
3.     Configure the time-offset threshold between the external reference clock and the PTP clock.
ptp alarm-threshold time-offset time-offset-value
By default, the time-offset threshold is 500 ns between the external reference clock and the PTP clock.
4.     Set the time-offset-sum peak-to-peak threshold.
ptp alarm-threshold time-offset-sum pk-pk threshold-value
By default, the time-offset-sum peak-to-peak threshold is 500 ns.
5.     Set the PTP time locking and unlocking thresholds.
ptp alarm-threshold { time-lock lock-value | time-unlock unlock-value } *
By default, the PTP time locking threshold is 200 ns and PTP time unlocking threshold is 300 ns.
This command is supported only in R3608 and later.
Display PTP clock information.
display ptp clock
Display the delay correction history.
display ptp corrections
Display information about foreign master nodes.
display ptp foreign-masters-record [ interface interface-type interface-number ]
Display PTP information for one or all PTP interfaces.
display ptp interface [ interface-type interface-number | brief ]
Display parent node information for the PTP device.
display ptp parent
Display brief information about the PTP synchronization path from the GM to the device.
display ptp path-trace
Display PTP statistics.
display ptp statistics [ interface interface-type interface-number ]
Display PTP clock time properties.
display ptp time-property
Clear PTP statistics.
reset ptp statistics [ interface interface-type interface-number ]
As shown in Figure 4, configure PTP (IEEE 1588 version 2, IEEE 802.3/Ethernet transport, multicast transmission) to enable time synchronization between Device A and Device C.
·     Specify the IEEE 1588 version 2 PTP profile for Device A, Device B, and Device C.
·     Use the IEEE 802.3/Ethernet transport protocol for PTP messages.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and E2ETC clock node type for Device B. All clock nodes elect a GM through BMC in the PTP domain.
·     Use the default Request_Response delay measurement mechanism on Device A and Device C.
Figure 4 Network diagram
IMPORTANT
IMPORTANT:
By default, interfaces on the device are disabled (in ADM or Administratively Down state). To have an interface operate, you must use the undo shutdown command to enable that interface.
1.     Configure Device A:
# Specify the IEEE 1588 version 2 PTP profile.
[DeviceA] ptp profile 1588v2
# Specify the OC clock node type.
[DeviceA] ptp mode oc
# Specify PTP for obtaining the time.
[DeviceA] clock protocol ptp
# Enable PTP on HundredGigE 1/0/1.
[DeviceA] interface hundredgige 1/0/1
[DeviceA-HundredGigE1/0/1] ptp enable
[DeviceA-HundredGigE1/0/1] quit
2.     Configure Device B:
[DeviceB] ptp profile 1588v2
# Specify the E2ETC clock node type.
[DeviceB] ptp mode e2etc
[DeviceB] clock protocol ptp
[DeviceB] interface hundredgige 1/0/1
[DeviceB-HundredGigE1/0/1] ptp enable
[DeviceB-HundredGigE1/0/1] quit
# Enable PTP on HundredGigE 1/0/2.
[DeviceB] interface hundredgige 1/0/2
[DeviceB-HundredGigE1/0/2] ptp enable
[DeviceB-HundredGigE1/0/2] quit
3.     Configure Device C:
<DeviceC> system-view
[DeviceC] ptp profile 1588v2
[DeviceC] ptp mode oc
[DeviceC] clock protocol ptp
[DeviceC] interface hundredgige 1/0/1
[DeviceC-HundredGigE1/0/1] ptp enable
[DeviceC-HundredGigE1/0/1] quit
When the network is stable, perform the following tasks:
·     Use the display ptp clock command to display PTP clock information.
·     Use the display ptp interface brief command to display brief PTP running information for all interfaces.
# Display PTP clock information on Device A.
[DeviceA] display ptp clock
PTP profile         : IEEE 1588 Version 2
PTP mode            : OC
Slave only          : No
Sync uncertain      : Disabled
Clock state         : Disabled
Clock ID            : 000FE2-FFFE-FF0000
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 1
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 65535
Offset from master : 0 (ns)
Mean path delay    : 0 (ns)
Steps removed      : 0
Local clock time   : Sun Jan 15 20:57:29 2019
Clock source info:
 Clock   Pri1 Pri2 Accuracy Class TimeSrc Direction In-Status Offset(log variance)
 Local   128  128  254      248   160     N/A       N/A       65535
 ToD0    128  128  32       6     32      In        Inactive  65535
 ToD1    128  128  32       6     32      N/A       Inactive  65535
# Display brief PTP running information for all interfaces on Device A.
[DeviceA] display ptp interface brief
Name         State         Delay mechanism  Clock step  Asymmetry correction
GE1/0/1      Master        E2E              Two         0
# Display PTP clock information on Device B.
[DeviceB] display ptp clock
PTP mode            : E2ETC
Slave only          : No
Clock ID            : 000FE2-FFFE-FF0001
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 2
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master : N/A
Mean path delay    : N/A
Steps removed      : N/A
Clock source info:
# Display brief PTP running information for all interfaces on Device B.
[DeviceB] display ptp interface brief
GE1/0/1      N/A           E2E              Two         0
GE1/0/2      N/A           E2E              Two         0
The output shows that Device A is elected as the GM, and HundredGigE1/0/1 on Device A is the master port.
As shown in Figure 5, configure PTP (IEEE 1588 version 2, IPv4 UDP transport, multicast transmission) to enable time synchronization between the devices.
·     Use the IPv4 UDP transport protocol for PTP messages.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and P2PTC clock node type for Device B. All clock nodes elect a GM through BMC in the PTP domain.
·     Specify the peer delay measurement mechanism (p2p) for Device A and Device C.
Figure 5 Network diagram
IMPORTANT
IMPORTANT:
# Configure the source IP address for multicast PTP messages transmitted over IPv4 UDP.
[DeviceA] ptp source 10.10.1.1
 # On HundredGigE 1/0/1, specify IPv4 UDP transport for PTP messages and the peer delay measurement mechanism (p2p), and enable PTP.
[DeviceA-HundredGigE1/0/1] ptp transport-protocol udp [DeviceA-HundredGigE1/0/1] ptp delay-mechanism p2p
# Specify the P2PTC clock node type.
[DeviceB] ptp mode p2ptc
[DeviceB] ptp source 10.10.2.1
# On HundredGigE 1/0/1, specify the IPv4 UDP transport protocol and enable PTP.
DeviceB-HundredGigE1/0/1] ptp transport-protocol udp
# On HundredGigE 1/0/2, specify the IPv4 UDP transport protocol and enable PTP.
[DeviceB-HundredGigE1/0/2] ptp transport-protocol udp
[DeviceC] ptp source 11.10.10.1
# On HundredGigE 1/0/1, specify the IPv4 UDP transport protocol and the peer delay measurement mechanism (p2p), and enable PTP.
[DeviceC-HundredGigE1/0/1] ptp transport-protocol udp [DeviceC-HundredGigE1/0/1] ptp delay-mechanism p2p
When the network is stable, perform the following tasks on Device A and Device B.
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
Local clock time   : Sun Jan 15 20:57:29 2011
Clock source info:
GE1/0/1      Master        P2P              Two         0
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : N/A
Clock source info:
GE1/0/1      N/A           P2P              Two         0
GE1/0/2      N/A           P2P              Two         0
As shown in Figure 6, configure PTP (IEEE 1588 version 2, IPv4 UDP encapsulation, unicast transmission) to enable Device A, Device B, Device C, and the base station to synchronize the time with the ToD clock source.
·     Specify the IEEE 1588 version 2 PTP profile and unicast IPv4 UDP transport of PTP messages for Device A, Device B, and Device C.
·     Assign Device A, Device B, Device C, and the base station to PTP domain 0. Specify the BC clock node type for Device A, Device B, and Device C.
·     Connect Device A to the ToD clock source and Device C to the base station.
·     All clock nodes in the PTP domain use the default Request_Response delay measurement mechanism.
Figure 6 Network diagram
IMPORTANT
IMPORTANT:
The device does not provide ToD interfaces. You can deploy it as Device B or C but not A.
1.     Assign IP addresses to the interfaces, and make sure the devices can reach each other, as shown in Figure 6. (Details not shown.)
2.     Configure Device A:
# Specify the BC clock node type.
[DeviceA] ptp mode bc
# Configure the device to receive ToD clock signals and set the delay time correction value to 1000 nanoseconds.
[DeviceA] ptp tod0 input delay 1000
# Set priority 1 to 0 for the ToD 0 clock.
[DeviceA] ptp priority clock-source tod0 priority1 0
# On HundredGigE 1/0/1, configure the destination IP address for unicast PTP messages transmitted over IPv4 UDP, and enable PTP.
[DeviceA-HundredGigE1/0/1] ptp unicast-destination 10.10.10.2
3.     Configure Device B:
[DeviceB] ptp mode bc
[DeviceB-HundredGigE1/0/1] ptp transport-protocol udp
[DeviceB-HundredGigE1/0/1] ptp unicast-destination 10.10.10.1
# On HundredGigE 1/0/2, configure the destination IP address for unicast PTP messages transmitted over IPv4 UDP, and enable PTP.
[DeviceB-HundredGigE1/0/2] ptp unicast-destination 11.10.10.1
4.     Configure Device C:
[DeviceC] ptp mode bc
# Create a PTP domain.
[DeviceC] ptp domain 0
[DeviceC-HundredGigE1/0/1] ptp unicast-destination 11.10.10.2
# On HundredGigE1/0/2, specify the IPv4 UDP transport protocol for PTP messages, configure the destination IP address for unicast PTP messages, and enable PTP.
[DeviceC] interface hundredgige 1/0/2
[DeviceC-HundredGigE1/0/2] ptp transport-protocol udp
[DeviceC-HundredGigE1/0/2] ptp unicast-destination 12.10.10.1
[DeviceC-HundredGigE1/0/2] ptp enable
[DeviceC-HundredGigE1/0/2] quit
5.     Configure the base station.
# Specify PTP domain 0.
# Specify the IPv4 UDP transport protocol for PTP messages.
# Set the destination IP address of unicast PTP messages to 12.10.10.2.
# Specify the Request_Response delay measurement mechanism.
For more information, see the configuration guide for the base station.
PTP mode            : BC
Slave only          : No
Clock type          : ToD0
 ToD direction  : In
 ToD delay time : 1000 (ns)
Clock domain        : 0
Priority1     : 0
Priority2     : 128
Clock quality :
 Class                 : 6
 Accuracy              : 32
Steps removed      : 0
Clock source info:
 ToD0    128  128  32       6     32      In        Active    65535
# Display PTP clock information on Device C.
[DeviceC] display ptp clock
PTP mode            : BC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master  : 106368539000 (ns)
Mean path delay     : 2791000 (ns)
Steps removed       : 2
Clock source info:
# Display brief PTP running information for all interfaces on Device C.
[DeviceC] display ptp interface brief
GE1/0/1      Slave         E2E              Two         0
GE1/0/2      Master        E2E              Two         0
As shown in Figure 7, configure PTP (IEEE 802.1AS, IEEE 802.3/Ethernet transport, multicast transmission) to enable time synchronization between Device A, Device B, and Device C.
·     Specify the IEEE 802.1AS PTP profile for Device A, Device B, and Device C.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and P2PTC clock node type for Device B. The clock nodes elect a GM through BMC in the PTP domain.
·     Use the default peer delay measurement mechanism on all clock nodes in the PTP domain.
Figure 7 Network diagram
IMPORTANT
IMPORTANT:
The IEEE 802.1AS PTP profile transports PTP messages over IEEE 802.3/Ethernet rather than IPv4 UDP and in multicast rather than unicast mode.
IMPORTANT
IMPORTANT:
# Specify the IEEE 802.1AS PTP profile.
[DeviceA] ptp profile 802.1AS
[DeviceB] ptp profile 802.1AS
# Specify the IEEE 1588 802.1AS PTP profile.
[DeviceC] ptp profile 802.1AS
PTP profile         : IEEE 802.1AS
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 246
Priority2     : 248
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 16640
Steps removed      : 0
Clock source info:
 ToD0    128  128  32       6     32      N/A       Inactive  65535
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 246
Priority2     : 248
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : N/A
Clock source info:
 ToD0    0    128  32       6     32      In        Inactive  65535