10-Layer 2—LAN Switching Command Reference
HomeSupportReference GuidesCommand ReferencesH3C SecPath M9000 Command Reference(V7)(R9153P39 R9001P39)-6W40010-Layer 2—LAN Switching Command Reference
03-VLAN commands
03-VLAN commands 131.34 KB
VLAN commands
Basic VLAN commands
bandwidth
Use bandwidth to set the expected bandwidth of an interface.
bandwidth bandwidth-value
undo bandwidth
VLAN interface view
context-admin
# Set the expected bandwidth to 10000 kbps for VLAN-interface 1.
[Sysname-Vlan-interface1] bandwidth 10000
default
Use default to restore the default settings for a VLAN interface.
default
VLAN interface view
context-admin
CAUTION
CAUTION:
The default command might interrupt ongoing network services. Make sure you are fully aware of the impact of this command when you use it on a live network.
This command might fail to restore the default settings for some commands for reasons such as command dependencies or system restrictions. Use the display this command in interface view to identify these commands, and then use their undo forms or follow the command reference to restore their default settings. If your restoration attempt still fails, follow the error message instructions to resolve the problem.
# Restore the default settings for VLAN-interface 1.
[Sysname-Vlan-interface1] default
description
Use description to configure the description of a VLAN or VLAN interface.
For a VLAN, the description is VLAN vlan-id. The vlan-id argument specifies the VLAN ID in a four-digit format. If the VLAN ID has fewer than four digits, leading zeros are added. For example, the default description of VLAN 100 is VLAN 0100.
For a VLAN interface, the description is the name of the interface. For example, Vlan-interface1 Interface.
VLAN view
VLAN interface view
context-admin
To manage VLANs and VLAN interfaces efficiently, configure descriptions for them based on their functions or connections.
# Configure the description of VLAN 2 as sales-private.
[Sysname] vlan 2
[Sysname-vlan2] description sales-private
# Configure the description of VLAN-interface 2 as linktoPC56.
[Sysname] vlan 2
[Sysname-vlan2] quit
[Sysname-Vlan-interface2] description linktoPC56
display interface vlan-interface
display vlan
Use display interface vlan-interface to display VLAN interface information.
display interface [ vlan-interface [ interface-number ] ] [ brief [ description | down ] ]
context-admin
context-operator
vlan-interface interface-number: Specifies a VLAN interface number. If you do not specify this option, the command displays information about all interfaces except VA interfaces. If you specify the vlan-interface keyword without specifying an interface, the command displays information about all VLAN interfaces. For more information about VA interfaces, see PPP in PPP and PPPoE Configuration Guide.
down: Displays VLAN interfaces in down state and their down causes. If you do not specify this keyword, the command displays information about VLAN interfaces in all states.
# Display information about VLAN-interface 2.
<Sysname> display interface vlan-interface 2
Vlan-interface2
Current state: DOWN
Line protocol state: DOWN
Description: Vlan-interface2 Interface
Bandwidth: 100000 kbps
Internet protocol processing : Disabled
IP packet frame type: Ethernet II, hardware address: 000f-e249-8050
IPv6 packet frame type: Ethernet II, hardware address: 000f-e249-8050
Output queue - Urgent queuing: Size/Length/Discards 0/1024/0
# Display brief information about VLAN-interface 2.
<Sysname> display interface vlan-interface 2 brief
Protocol: (s) - spoofing
Interface            Link Protocol Primary IP         Description
Vlan2                DOWN DOWN     --
Vlan-interface2
VLAN interface name.
Current state
Physical link state of the VLAN interface:
·     Administratively DOWN—The interface has been shut down by using the shutdown command.
·     DOWN—The interface is administratively up, but its physical state is down. The VLAN of this VLAN interface does not contain any physical ports in up state. The ports might not be connected correctly or the links might have failed.
·     UP—The interface is both administratively and physically up.
Line protocol state
Data link layer state of the VLAN interface:
·     DOWN—The link layer protocol state of the interface is down.
·     UP—The link layer protocol state of the interface is up.
Description of the VLAN interface.
Bandwidth
Expected bandwidth of the VLAN interface.
MTU of the VLAN interface.
The VLAN interface is not assigned an IP address and cannot process IP packets.
IPv4 packet framing format.
hardware address
MAC address of the VLAN interface.
IPv6 packet framing format.
Information about the urgent, protocol, and FIFO output queues:
·     Size—Number of packets in the queue.
·     Length—Maximum number of packets that the queue can contain.
·     Discards—Number of dropped packets.
The most recent time that the reset counters interface vlan-interface command was executed. This field displays Never if you have never executed this command.
Average rates of input packets and output packets in the last 300 seconds (in Bps, bps, and pps).
Total number and size (in bytes) of the received packets of the interface and the number of the dropped packets.
Total number and size (in bytes) of the sent packets of the interface and the number of the dropped packets.
Brief information about Layer 3 interfaces.
Abbreviated interface name.
Physical link state of the interface:
·     UP—The interface is physically up.
·     DOWN—The interface is physically down.
·     ADM—The interface has been shut down by using the shutdown command. To restore the physical state of the interface, use the undo shutdown command.
Protocol
Data link layer protocol state of the interface:
·     UP—The data link layer protocol state of the interface is up.
·     DOWN—The data link layer protocol state of the interface is down.
·     UP(s)—The data link layer protocol of the interface is up, but the link is an on-demand link or does not exist. The (s) attribute represents the spoofing flag.
Primary IP
Primary IP address of the interface.
display vlan
Use display vlan to display VLAN information.
display vlan [ vlan-id1 [ to vlan-id2 ] | all | dynamic | static ]
context-admin
context-operator
vlan-id1: Specifies a VLAN by its ID in the range of 1 to 4094.
vlan-id1 to vlan-id2: Specifies a VLAN ID range. Both the vlan-id1 and the vlan-id2 arguments are in the range of 1 to 4094. The value for the vlan-id2 argument must be equal to or greater than the value for the vlan-id1 argument.
all: Specifies all VLANs.
dynamic: Specifies dynamic VLANs. If you specify this keyword, the command displays the total number of dynamic VLANs and each dynamic VLAN ID. Dynamic VLANs are assigned by a RADIUS server.
static: Specifies static VLANs. If you specify this keyword, the command displays the total number of static VLANs and each static VLAN ID. Static VLANs are manually created.
# Display information about VLAN 2.
<Sysname> display vlan 2
 VLAN ID: 2
 VLAN type: Static
 Description: VLAN 0002
 Tagged ports:   None
 Untagged ports:
    GigabitEthernet1/0/1  GigabitEthernet1/0/2  GigabitEthernet1/0/3
# Display information about VLAN 3.
<Sysname> display vlan 3
 VLAN ID: 3
 VLAN type: static
 Route interface: Configured
 IPv4 address: 1.1.1.1
 IPv4 subnet mask: 255.255.255.0
 Description: VLAN 0003
 Tagged ports:   None
 Untagged ports: None
VLAN type
VLAN type, static or dynamic.
Route interface
Whether the VLAN interface is configured for the VLAN.
·     Not configured.
·     Configured.
Description of the VLAN.
Name
VLAN name.
IP address
Primary IPv4 address of the VLAN interface. This field is displayed only when an IPv4 address is configured for the VLAN interface.
When the VLAN interface is also configured with secondary IPv4 addresses, you can view them by using one of the following commands:
·     display interface vlan-interface.
·     display this (VLAN interface view).
Subnet mask
Subnet mask of the primary IP address. This field is available only when an IP address is configured for the VLAN interface.
Tagged ports
Tagged members of the VLAN.
Untagged ports
Untagged members of the VLAN.
vlan
display vlan brief
Use display vlan brief to display brief VLAN information.
display vlan brief
context-admin
context-operator
# Display brief VLAN information.
<Sysname> display vlan brief
Brief information about all VLANs:
Supported Minimum VLAN ID: 1
Supported Maximum VLAN ID: 4094
Default VLAN ID: 1
VLAN ID   Name                             Port
1         VLAN 0001                        GE1/0/1  GE1/0/2  GE1/0/3  GE1/0/4
                                           GE1/0/5  GE1/0/6
2         VLAN 0002
3         VLAN 0003
Default VLAN ID
System default VLAN ID.
Name
VLAN name.
Port
Ports that allow packets from the VLAN to pass through.
Use interface vlan-interface to create a VLAN interface and enter its view, or enter the view of an existing VLAN interface.
Use undo interface vlan-interface to delete a VLAN interface.
undo interface vlan-interface interface-number
No VLAN interfaces exist.
context-admin
interface-number: Specifies a VLAN interface number in the range of 1 to 4094.
Create the VLAN before you create the VLAN interface for a VLAN.
# Create VLAN-interface 2, and enter its view.
[Sysname] vlan 2
mtu
Use mtu to set the MTU for a VLAN interface.
mtu size
undo mtu
The MTU of a VLAN interface is 1500 bytes.
VLAN interface view
context-admin
size: Sets the MTU in the range of 46 to 9198 bytes.
If you configure both the mtu and ip mtu commands on a VLAN interface, the MTU set by the ip mtu command is used for fragmentation. For more information about the ip mtu command, see Layer 3—IP Services Command Reference.
# Set the MTU to 1492 bytes for VLAN-interface 1.
[Sysname-Vlan-interface1] mtu 1492
name
Use name to assign a name to a VLAN.
Use undo name to restore the default.
name text
undo name
The name of a VLAN is VLAN vlan-id. The vlan-id argument specifies the VLAN ID in a four-digit format. If the VLAN ID has fewer than four digits, leading zeros are added. For example, the name of VLAN 100 is VLAN 0100.
VLAN view
context-admin
text: Specifies a VLAN name, a case-sensitive string of 1 to 32 characters.
If a large number of VLANs are configured, use VLAN names to identify them.
# Assign the name test vlan to VLAN 2.
[Sysname] vlan 2
[Sysname-vlan2] name test vlan
display vlan
Use reset counters interface vlan-interface to clear statistics on a VLAN interface.
reset counters interface [ vlan-interface [ interface-number ] ]
context-admin
vlan-interface interface-number: Specifies a VLAN interface by its number. If you do not specify this option, this command clears statistics on all interfaces except VA interfaces. If you specify the vlan-interface keyword without specifying an interface, this command clears statistics on all VLAN interfaces.
Use this command to clear the history statistics before you collect statistics within a time period.
# Clear statistics on VLAN-interface 2.
<Sysname> reset counters interface vlan-interface 2
shutdown
Use shutdown to shut down a VLAN interface.
Use undo shutdown to bring up a VLAN interface.
shutdown
A VLAN interface is not manually shut down.
VLAN interface view
context-admin
When a VLAN interface is not manually shut down, the following guidelines apply to the interface state:
·     The VLAN interface is down if all ports in the VLAN are down.
·     The VLAN interface is up if one or more ports in the VLAN are up.
When you use this command to shut down a VLAN interface, the VLAN interface remains in DOWN (Administratively) state. In this case, the VLAN interface state is not affected by the state of the ports in the VLAN.
Before you configure parameters for a VLAN interface, use this command to shut it down to prevent the configuration from affecting the network. After you complete the VLAN interface configuration, use the undo shutdown command to make the settings take effect.
To troubleshoot a failed VLAN interface, you can use the shutdown command and then the undo shutdown command on the interface to see whether it recovers.
In a VLAN, the state of each Ethernet port is independent of the state of the VLAN interface.
# Shut down VLAN-interface 2, and then bring it up.
[Sysname-Vlan-interface2] shutdown
[Sysname-Vlan-interface2] undo shutdown
vlan
Use vlan vlan-id to create a VLAN and enter its view, or enter the view of an existing VLAN.
Use vlan vlan-id1 to vlan-id2 to create VLANs vlan-id1 through vlan-id2, except reserved VLANs.
Use vlan all to create VLANs 1 through 4094.
Use undo vlan to delete the specified VLANs.
vlan { vlan-id1 [ to vlan-id2 ] | all }
undo vlan { vlan-id1 [ to vlan-id2 ] | all }
VLAN 1 (system default VLAN) exists.
context-admin
vlan-id1: Specifies a VLAN ID in the range of 1 to 4094.
vlan-id1 to vlan-id2: Specifies a VLAN range. The vlan-id1 and vlan-id2 arguments specify VLAN IDs. The value range for each of the two arguments is 1 to 4094. The value for the vlan-id2 argument must be equal to or greater than the value for the vlan-id1 argument.
all: Specifies all VLANs except reserved VLANs. The keyword is not supported when the maximum number of VLANs that can be created on a device is less than 4094.
You cannot create or delete the system default VLAN (VLAN 1) or reserved VLANs.
Before you delete a dynamic VLAN or a VLAN locked by an application, you must first remove the configuration from the VLAN.
# Create VLAN 2 and enter its view.
[Sysname] vlan 2
[Sysname-vlan2]
# Create VLANs 4 through 100.
[Sysname] vlan 4 to 100
display vlan
vlan-strip enable
Use vlan-strip enable to configure an interface to strip VLAN tags of received packets.
Use undo vlan-strip enable to restore the default.
vlan-strip enable
An interface does not strip VLAN tags of received packets.
context-admin
This command is supported only by VF interfaces of Intel 82599 NICs when the PF driver is open-source on the host side.
# Configure GigabitEthernet 1/0/1 to strip VLAN tags of received packets.
[Sysname-GigabitEthernet1/0/1] vlan-strip enable
Port-based VLAN commands
display port
Use display port to display information about hybrid or trunk ports.
context-admin
context-operator
hybrid: Specifies hybrid ports.
trunk: Specifies trunk ports.
# Display information about hybrid ports.
<Sysname> display port hybrid
Interface            PVID  VLAN Passing
GE1/0/1              100   Tagged:  1000, 1002, 1500, 1600-1611, 2000,
                                    2555-2558, 3000, 4000
                           Untagged:1, 10, 15, 18, 20-30, 44, 55, 67, 100,
                                    150-160, 200, 255, 286, 300-302
# Display information about trunk ports.
<Sysname> display port trunk
GE1/0/2              2     1-4, 6-100, 145, 177, 189-200, 244, 289, 400,
                           555, 600-611, 1000, 2006-2008
Interface name.
PVID
Port VLAN ID.
VLAN Passing
Existing VLANs allowed on the port.
Tagged
VLANs from which the port sends packets without removing VLAN tags.
Untagged
VLANs from which the port sends packets after removing VLAN tags.
port
Use port to assign the specified access ports to a VLAN.
Use undo port to remove the specified access ports from a VLAN.
port interface-list
undo port interface-list
All ports are in VLAN 1.
VLAN view
context-admin
interface-list: Specifies a space-separated list of up to 10 Ethernet interface items. Each item specifies an Ethernet interface or a range of Ethernet interfaces in the form of interface-type interface-number1 to interface-type interface-number2. The value for the interface-number2 argument must be equal to or greater than the value for the interface-number1 argument.
This command is applicable only to access ports. This command cannot assign access ports to or remove access ports from VLAN 1.
By default, all ports are access ports. You can manually configure the port link type. For more information, see "port link-type."
# Assign GigabitEthernet 1/0/1 through GigabitEthernet 1/0/2 to VLAN 2.
[Sysname] vlan 2
[Sysname-vlan2] port gigabitethernet 1/0/1 to gigabitethernet 1/0/2
display vlan
port access vlan
Use port access vlan to assign an access port to the specified VLAN.
Use undo port access vlan to restore the default.
port access vlan vlan-id
All access ports belong to VLAN 1.
context-admin
vlan-id: Specifies a VLAN by its ID in the range of 1 to 4094.
By default, all access ports belong to VLAN 1. Therefore, this command cannot be used to assign access ports to VLAN 1. To move an access port to VLAN 1, execute the undo port access vlan command on the access port.
Before assigning an access port to a VLAN, make sure the VLAN has been created.
# Assign GigabitEthernet 1/0/1 to VLAN 3.
[Sysname] vlan 3
[Sysname-vlan3] quit
[Sysname-GigabitEthernet1/0/1] port access vlan 3
port hybrid pvid
Use port hybrid pvid to set the PVID of a hybrid port.
Use undo port hybrid pvid to set the PVID of a hybrid port to 1.
port hybrid pvid vlan vlan-id
The PVID of a hybrid port is the ID of the VLAN to which the port belongs when its link type is access.
context-admin
You can use a nonexistent VLAN as the PVID of a hybrid port. When you delete the PVID of a hybrid port by using the undo vlan command, the PVID setting of the port does not change.
For correct packet transmission, set the same PVID for a local hybrid port and its peer.
To enable a hybrid port to transmit packets from its PVID, you must assign the hybrid port to the PVID by using the port hybrid vlan command.
# Configure GigabitEthernet 1/0/1 as a hybrid port, set its PVID to VLAN 100, and assign it to VLAN 100 as an untagged member.
[Sysname] vlan 100
[Sysname-vlan100] quit
[Sysname-GigabitEthernet1/0/1] port link-type hybrid
[Sysname-GigabitEthernet1/0/1] port hybrid pvid vlan 100
[Sysname-GigabitEthernet1/0/1] port hybrid vlan 100 untagged
port hybrid vlan
port link-type
port hybrid vlan
Use port hybrid vlan to assign a hybrid port to the specified VLANs.
Use undo port hybrid vlan to remove a hybrid port from the specified VLANs.
undo port hybrid vlan vlan-id-list
A hybrid port is an untagged member of the VLAN to which the port belongs when its link type is access.
context-admin
vlan-id-list: Specifies a space-separated list of up to 10 VLAN items. Each item specifies a VLAN ID or a range of VLAN IDs in the form of vlan-id1 to vlan-id2. The value range for VLAN IDs is 1 to 4094. The value for the vlan-id2 argument must be equal to or greater than the value for the vlan-id1 argument. The specified VLANs must already exist on the device.
tagged: Configures the port as a tagged member of the specified VLANs. A tagged member of a VLAN sends packets from the VLAN without removing VLAN tags.
untagged: Configures the port as an untagged member of the specified VLANs. An untagged member of a VLAN sends packets from the VLAN after removing VLAN tags.
A hybrid port can allow multiple VLANs. If you execute this command multiple times on a hybrid port, the hybrid port allows all the specified VLANs.
# Configure GigabitEthernet 1/0/1 as a hybrid port, and assign it to VLAN 2, VLAN 4, and VLAN 50 through VLAN 100 as a tagged member.
[Sysname-GigabitEthernet1/0/1] port hybrid vlan 2 4 50 to 100 tagged
port link-type
port link-type
Use port link-type to set the link type of a port.
Use undo port link-type to restore the default link type of a port.
undo port link-type
Each port is an access port.
context-admin
access: Sets the port link type to access.
hybrid: Sets the port link type to hybrid.
trunk: Sets the port link type to trunk.
To change the link type of a port from trunk to hybrid or vice versa, first set the link type to access.
# Configure GigabitEthernet 1/0/1 as a trunk port.
port trunk permit vlan
Use port trunk permit vlan to assign a trunk port to the specified VLANs.
Use undo port trunk permit vlan to remove a trunk port from the specified VLANs.
undo port trunk permit vlan { vlan-id-list | all }
A trunk port allows packets only from VLAN 1 to pass through.
context-admin
all: Specifies all VLANs. To prevent unauthorized VLAN users from accessing restricted resources through the port, use the port trunk permit vlan all command with caution.
A trunk port can allow multiple VLANs. If you execute this command multiple times on a trunk port, the trunk port allows all the specified VLANs.
On a trunk port, packets only from the PVID can pass through untagged.
# Configure GigabitEthernet 1/0/1 as a trunk port, and assign it to VLAN 2, VLAN 4, and VLAN 50 through VLAN 100.
[Sysname-GigabitEthernet1/0/1] port trunk permit vlan 2 4 50 to 100
port link-type
port trunk pvid
Use port trunk pvid to set the PVID for a trunk port.
Use undo port trunk pvid to restore the default.
port trunk pvid vlan vlan-id
The PVID of a trunk port is VLAN 1.
context-admin
You can use a nonexistent VLAN as the PVID for a trunk port. When you delete the PVID of a trunk port by using the undo vlan command, the PVID setting of the port does not change.
For correct packet transmission, set the same PVID for a local trunk port and its peer.
To enable a trunk port to transmit packets from its PVID, you must assign the trunk port to the PVID by using the port trunk permit vlan command.
# Configure GigabitEthernet 1/0/1 as a trunk, set its PVID to VLAN 100, and assign it to VLAN 100.
[Sysname-GigabitEthernet1/0/1] port trunk pvid vlan 100
[Sysname-GigabitEthernet1/0/1] port trunk permit vlan 100
port link-type
VLAN group commands
display vlan-group
Use display vlan-group to display VLAN group information.
display vlan-group [ group-name ]
context-admin
context-operator
group-name: Specifies a VLAN group by its name, a case-sensitive string of 1 to 31 characters. The first character must be an alphabetical character. If you do not specify this argument, the command displays information about all VLAN groups.
# Display information about VLAN group test001.
<Sysname> display vlan-group test001
VLAN group: test001
     VLAN list: 2-4 100 200
# Display information about all VLAN groups.
VLAN group: rnd
     VLAN list: Null
VLAN group: test001
Table 5 Command output
VLAN group
Name of the VLAN group.
VLAN list
VLAN list in the VLAN group.
vlan-group
vlan-list
vlan-group
Use vlan-group to create a VLAN group and enter its view, or enter the view of an existing VLAN group.
Use undo vlan-group to delete a VLAN group.
vlan-group group-name
undo vlan-group group-name
No VLAN groups exist.
context-admin
A VLAN group includes a set of VLANs. You can add multiple VLAN lists to a VLAN group.
# Create a VLAN group named test001 and enter VLAN group view.
[Sysname] vlan-group test001
[Sysname-vlan-group-test001]
vlan-list
vlan-list
Use vlan-list to add VLANs to a VLAN group.
Use undo vlan-list to remove VLANs from a VLAN group.
vlan-list vlan-id-list
undo vlan-list vlan-id-list
No VLANs exist in a VLAN group.
VLAN group view
context-admin
# Add VLAN 2 through VLAN 4, VLAN 100, and VLAN 200 to VLAN group test001.
[Sysname-vlan-group-test001] vlan-list 2 to 4 100 200
vlan-group