08-ACL and QoS Configuration Guide
HomeSupportSwitchesS6860 SeriesConfigure & DeployConfiguration GuidesH3C S6860 Switch Series Configuration Guide-Release 26xx-6W10308-ACL and QoS Configuration Guide
01-ACL configuration
01-ACL configuration 151.42 KB
Configuring ACLs
Overview
An access control list (ACL) is a set of rules for identifying traffic based on criteria such as source IP address, destination IP address, and port number. The rules are also called permit or deny statements.
ACLs are primarily used for packet filtering. "Configuring packet filtering with ACLs" provides an example. You can use ACLs in QoS, security, routing, and other modules for identifying traffic. The packet drop or forwarding decisions depend on the modules that use ACLs.
ACL types
ACL number
IP version
Match criteria
Basic ACLs
2000 to 2999
IPv4
Source IPv4 address.
IPv6
Source IPv6 address.
Advanced ACLs
3000 to 3999
IPv4
Source IPv4 address, destination IPv4 address, packet priority, protocol number, and other Layer 3 and Layer 4 header fields.
IPv6
Source IPv6 address, destination IPv6 address, packet priority, protocol number, and other Layer 3 and Layer 4 header fields.
Layer 2 ACLs
4000 to 4999
IPv4 and IPv6
Layer 2 header fields, such as source and destination MAC addresses, 802.1p priority, and link layer protocol type.
User-defined ACLs
5000 to 5999
IPv4 and IPv6
User specified matching patterns in protocol headers.
Numbering and naming ACLs
When creating an ACL, you must assign it a number or name for identification. You can specify an existing ACL by its number or name. Each ACL type has a unique range of ACL numbers.
For an IPv4 basic or advanced ACL, its ACL number or name must be unique in IPv4. For an IPv6 basic or advanced ACL, its ACL number and name must be unique in IPv6. For an ACL of some other type, its number or name must be globally unique.
Match order
The rules in an ACL are sorted in a specific order. When a packet matches a rule, the device stops the match process and performs the action defined in the rule. If an ACL contains overlapping or conflicting rules, the matching result and action to take depend on the rule order.
The following ACL match orders are available:
·           config—Sorts ACL rules in ascending order of rule ID. A rule with a lower ID is matched before a rule with a higher ID. If you use this method, check the rules and their order carefully.
The match order of user-defined ACLs can only be config.
·           auto—Sorts ACL rules in depth-first order. Depth-first ordering makes sure any subset of a rule is always matched before the rule. Table 1 lists the sequence of tie breakers that depth-first ordering uses to sort rules for each type of ACL.
Table 1 Sort ACL rules in depth-first order
ACL type
Sequence of tie breakers
IPv4 basic ACL
1.      VPN instance.
2.      More 0s in the source IPv4 address wildcard (more 0s means a narrower IPv4 address range).
3.      Rule configured earlier.
IPv4 advanced ACL
1.      VPN instance.
2.      Specific protocol number.
3.      More 0s in the source IPv4 address wildcard mask.
4.      More 0s in the destination IPv4 address wildcard.
5.      Narrower TCP/UDP service port number range.
6.      Rule configured earlier.
IPv6 basic ACL
1.      VPN instance.
2.      Longer prefix for the source IPv6 address (a longer prefix means a narrower IPv6 address range).
IPv6 advanced ACL
1.      VPN instance.
3.      Longer prefix for the source IPv6 address.
4.      Longer prefix for the destination IPv6 address.
Layer 2 ACL
1.      More 1s in the source MAC address mask (more 1s means a smaller MAC address).
2.      More 1s in the destination MAC address mask.
A wildcard mask, also called an inverse mask, is a 32-bit binary number represented in dotted decimal notation. In contrast to a network mask, the 0 bits in a wildcard mask represent "do care" bits, and the 1 bits represent "don't care" bits. If the "do care" bits in an IP address are identical to the "do care" bits in an IP address criterion, the IP address matches the criterion. All "don't care" bits are ignored. The 0s and 1s in a wildcard mask can be noncontiguous. For example, 0.255.0.255 is a valid wildcard mask.
Rule numbering
ACL rules can be manually numbered or automatically numbered. This section describes how automatic ACL rule numbering works.
Rule numbering step
If you do not assign an ID to the rule you are creating, the system automatically assigns it a rule ID. The rule numbering step sets the increment by which the system automatically numbers rules. For example, the default ACL rule numbering step is 5. If you do not assign IDs to rules you are creating, they are automatically numbered 0, 5, 10, 15, and so on. The wider the numbering step, the more rules you can insert between two rules.
By introducing a gap between rules rather than contiguously numbering rules, you have the flexibility of inserting rules in an ACL. This feature is important for a config-order ACL, where ACL rules are matched in ascending order of rule ID.
Automatic rule numbering and renumbering
The ID automatically assigned to an ACL rule takes the nearest higher multiple of the numbering step to the current highest rule ID, starting with 0.
For example, if the step is 5, and there are five rules numbered 0, 5, 9, 10, and 12, the newly defined rule is numbered 15. If the ACL does not contain a rule, the first rule is numbered 0.
Whenever the step changes, the rules are renumbered, starting from 0. For example, changing the step from 5 to 2 renumbers rules 5, 10, 13, and 15 as rules 0, 2, 4, and 6.
Fragment filtering with ACLs
Traditional packet filtering matches only first fragments of packets, and allows all subsequent non-first fragments to pass through. Attackers can fabricate non-first fragments to attack networks.
To avoid risks, the ACL feature is designed as follows:
·           Filters all fragments by default, including non-first fragments.
·           Allows for matching criteria modification for efficiency. For example, you can configure the ACL to filter only non-first fragments.
ACL configuration restrictions and guidelines
·           To create a numbered ACL, you can use one of the following command forms:
¡  acl [ ipv6 ] number acl-number
¡  acl { [ ipv6 ]  { advanced | basic } | mac | user-defined } acl-number
·           For a named ACL, you can enter the view of the ACL only by using the acl { [ ipv6 ]  { advanced | basic } | mac | user-defined } name acl-name command.
·           For a numbered ACL, you can enter the view of the ACL by using the acl [ ipv6 ] number acl-number or acl [ ipv6 | mac | user-defined ] acl-number command.
·           Matching packets are forwarded through slow forwarding if an ACL rule contains match criteria or has functions enabled in addition to the following match criteria and functions:
¡  Source and destination IP addresses.
¡  Source and destination ports.
¡  Transport layer protocol.
¡  ICMP or ICMPv6 message type, message code, and message name.
¡  VPN instance.
¡  Logging.
¡  Time range.
Slow forwarding requires packets to be sent to the control plane for forwarding entry calculation, which affects the device forwarding performance.
·           On a border gateway in a VXLAN or EVPN network, an ACL applied to a Layer 3 Ethernet interface or Layer 3 aggregate interface matches the packets on both the interface and its subinterfaces. For information about VXLAN and EVPN, see VXLAN Configuration Guide and EVPN Configuration Guide.
Configuration task list
Tasks at a glance
(Required.) Configure ACLs according to the characteristics of the packets to be matched:
·           Configuring a basic ACL
¡  Configuring an IPv4 basic ACL
¡  Configuring an IPv6 basic ACL
·           Configuring an advanced ACL
¡  Configuring an IPv4 advanced ACL
¡  Configuring an IPv6 advanced ACL
·           Configuring a Layer 2 ACL
·           Configuring a user-defined ACL
(Optional.) Copying an ACL
(Optional.) Configuring packet filtering with ACLs
This section describes procedures for configuring IPv4 and IPv6 basic ACLs.
IPv4 basic ACLs match packets based only on source IP addresses.
To configure an IPv4 basic ACL:
Step
Remarks
1.      Enter system view.
N/A
2.      Create an IPv4 basic ACL and enter its view.
acl basic { acl-number | name acl-name } [ match-order { auto | config } ]
acl { name acl-name | number acl-number [ name acl-name ] [ match-order { auto | config } ] }
By default, no ACLs exist.
The value range for a numbered IPv4 basic ACL is 2000 to 2999.
3.      (Optional.) Configure a description for the IPv4 basic ACL.
By default, an IPv4 basic ACL does not have a description.
4.      (Optional.) Set the rule numbering step.
step step-value [ start start-value ]
By default, the rule numbering step is 5 and the start rule ID is 0.
5.      Create or edit a rule.
rule [ rule-id ] { deny | permit } [ counting | fragment | logging | source { source-address source-wildcard | any } | time-range time-range-name | vpn-instance vpn-instance-name ] *
By default, no IPv4 basic ACL rules exist.
The logging keyword takes effect only when the module (for example, packet filtering) that uses the ACL supports logging.
6.      (Optional.) Add or edit a rule comment.
rule rule-id comment text
By default, no rule comment is configured.
IPv6 basic ACLs match packets based only on source IP addresses.
To configure an IPv6 basic ACL:
Step
Remarks
N/A
2.      Create an IPv6 basic ACL view and enter its view.
acl ipv6 basic { acl-number | name acl-name } [ match-order { auto | config } ]
acl ipv6 { name acl-name | number acl-number [ name acl-name ] [ match-order { auto | config } ] }
The value range for a numbered IPv6 basic ACL is 2000 to 2999.
3.      (Optional.) Configure a description for the IPv6 basic ACL.
By default, an IPv6 basic ACL does not have a description.
rule [ rule-id ] { deny | permit } [ counting | fragment | logging | routing [ type routing-type ] | source { source-address source-prefix | source-address/source-prefix | any } | time-range time-range-name | vpn-instance vpn-instance-name ] *
By default, no IPv6 basic ACL rules exist.
This section describes procedures for configuring IPv4 and IPv6 advanced ACLs.
IPv4 advanced ACLs match packets based on the following criteria:
·           Source IP addresses.
·           Destination IP addresses.
·           Packet priorities.
·           Local QoS IDs.
·           Protocol numbers.
·           Other protocol header information, such as TCP/UDP source and destination port numbers, TCP flags, ICMP message types, and ICMP message codes.
Compared to IPv4 basic ACLs, IPv4 advanced ACLs allow more flexible and accurate filtering.
To configure an IPv4 advanced ACL:
Step
Remarks
N/A
2.      Create an IPv4 advanced ACL and enter its view.
acl advanced { acl-number | name acl-name } [ match-order { auto | config } ]
The value range for a numbered IPv4 advanced ACL is 3000 to 3999.
3.      (Optional.) Configure a description for the IPv4 advanced ACL.
By default, an IPv4 advanced ACL does not have a description.
rule [ rule-id ] { deny | permit } protocol [ { { ack ack-value | fin fin-value | psh psh-value | rst rst-value | syn syn-value | urg urg-value } * | established } | counting | destination { dest-address dest-wildcard | any } | destination-port operator port1 [ port2 ] | { dscp dscp | { precedence precedence | tos tos } * } | fragment | icmp-type { icmp-type [ icmp-code ] | icmp-message } | logging | qos-local-id local-id-value | source { source-address source-wildcard | any } | source-port operator port1 [ port2 ] | time-range time-range-name | vpn-instance vpn-instance-name ] *
rule [ rule-id ] { deny | permit } vxlan [ destination { dest-address dest-wildcard | any } | source { source-address source-wildcard | any } | source-port operator port1 [ port2 ] | vxlan-id vxlan-id ] * inner-protocol inner-protocol [ counting | inner-destination { dest-address dest-wildcard | any } | inner-destination-port operator port1 [ port2 ] | inner-established | inner-source { source-address source-wildcard | any } | inner-source-port operator port1 [ port2 ] | logging | time-range time-range-name ] *
By default, no IPv4 advanced ACL rules exist.
IPv6 advanced ACLs match packets based on the following criteria:
·           Source IPv6 addresses.
·           Destination IPv6 addresses.
·           Local QoS IDs.
·           Protocol numbers.
·           Other protocol header fields such as the TCP/UDP source port number, TCP/UDP destination port number, ICMPv6 message type, and ICMPv6 message code.
Compared to IPv6 basic ACLs, IPv6 advanced ACLs allow more flexible and accurate filtering.
To configure an IPv6 advanced ACL:
Step
Remarks
N/A
2.      Create an IPv6 advanced ACL and enter its view.
acl ipv6 advanced { acl-number | name acl-name } [ match-order { auto | config } ]
The value range for a numbered IPv6 advanced ACL is 3000 to 3999.
3.      (Optional.) Configure a description for the IPv6 advanced ACL.
By default, an IPv6 advanced ACL does not have a description.
rule [ rule-id ] { deny | permit } protocol [ { { ack ack-value | fin fin-value | psh psh-value | rst rst-value | syn syn-value | urg urg-value } * | established } | counting | destination { dest-address dest-prefix | dest-address/dest-prefix | any } | destination-port operator port1 [ port2 ] | dscp dscp | flow-label flow-label-value | fragment | icmp6-type { icmp6-type icmp6-code | icmp6-message } | logging | qos-local-id local-id-value | routing [ type routing-type ] | hop-by-hop [ type hop-type ] | source { source-address source-prefix | source-address/source-prefix | any } | source-port  | time-range time-range-name | vpn-instance vpn-instance-name ] *
By default, no IPv6 advanced ACL rules exist.
Layer 2 ACLs, also called "Ethernet frame header ACLs," match packets based on Layer 2 Ethernet header fields, such as:
·           Source MAC address.
·           Destination MAC address.
·           802.1p priority (VLAN priority).
·           Link layer protocol type.
·           Encapsulation type.
·           Inner source MAC address.
·           Inner destination MAC address.
·           Inner link layer protocol type.
To configure a Layer 2 ACL:
Step
Remarks
N/A
2.      Create a Layer 2 ACL and enter its view.
acl mac { acl-number | name acl-name } [ match-order { auto | config } ]
The value range for a numbered Layer 2 ACL is 4000 to 4999.
3.      (Optional.) Configure a description for the Layer 2 ACL.
By default, a Layer 2 ACL does not have a description.
rule [ rule-id ] { deny | permit } [ cos dot1p | counting | dest-mac dest-address dest-mask | { lsap lsap-type lsap-type-mask | type protocol-type protocol-type-mask } | source-mac source-address source-mask | time-range time-range-name ] *
rule [ rule-id ] { deny | permit } vxlan [ counting | dest-mac dest-address dest-mask | inner-dest-mac inner-dest-address inner-dest-mask | inner-source-mac inner-source-address inner-source-mask | inner-type inner-protocol-type inner-protocol-type-mask | source-mac source-address source-mask | time-range time-range-name | type protocol-type protocol-type-mask | vxlan-id vxlan-id ] *
By default, no Layer 2 ACL rules exist.
To specify the lsap lsap-type lsap-type-mask option in an ACL used in a QoS policy or packet filter, you must specify AAAA and FFFF for the lsap-type and lsap-type-mask arguments, respectively.
User-defined ACLs allow you to customize rules based on information in protocol headers. You can define a user-defined ACL to match packets. A specific number of bytes after an offset (relative to the specified header) are compared against a match pattern after being ANDed with a match pattern mask.
To configure a user-defined ACL:
Step
Remarks
N/A
2.      Create a user-defined ACL and enter its view.
acl user-defined { acl-number | name acl-name }
acl number acl-number [ name acl-name ]
The value range for a numbered user-defined ACL is 5000 to 5999.
3.      (Optional.) Configure a description for the user-defined ACL.
By default, a user-defined ACL does not have a description.
4.      Create or edit a rule.
rule [ rule-id ] { deny | permit } [ { { l2 I l4 } rule-string rule-mask offset }&<1-8> ] [ counting | time-range time-range-name ] *
By default, no user-defined ACL rules exist.
5.      (Optional.) Add or edit a rule comment.
Copying an ACL
You can create an ACL by copying an existing ACL (source ACL). The new ACL (destination ACL) has the same properties and content as the source ACL, but uses a different number or name than the source ACL.
To successfully copy an ACL, make sure:
·           The destination ACL number is from the same type as the source ACL number.
·           The source ACL already exists, but the destination ACL does not.
To copy an ACL:
Step
2.      Copy an existing ACL to create a new ACL.
acl [ ipv6 | mac | user-defined ] copy { source-acl-number | name source-acl-name } to { dest-acl-number | name dest-acl-name }
This section describes procedures for using an ACL to filter packets. For example, you can apply an ACL to an interface to filter incoming or outgoing packets.
Applying an ACL to an interface for packet filtering
The term "interface" in this section collectively refers to Layer 2 Ethernet interfaces, Layer 2 aggregate interfaces, Layer 3 Ethernet interfaces, Layer 3 aggregate interfaces, Layer 3 Ethernet subinterfaces, VLAN interfaces, VSI interfaces, S-channel interfaces, and S-channel aggregate interfaces. You can use the port link-mode command to configure an Ethernet port as a Layer 2 or Layer 3 interface (see Layer 2—LAN Switching Configuration Guide). For information about VSI interfaces, see VXLAN Configuration Guide. For information about S-channel interfaces and S-channel aggregate interfaces, see EVB Configuration Guide.
To apply an ACL to an interface for packet filtering:
Step
Remarks
N/A
2.      Enter interface view.
N/A
3.      Apply an ACL to the interface to filter packets.
packet-filter [ ipv6 | mac | user-defined ] { acl-number | name acl-name } { inbound | outbound } [ hardware-count ] [ share-mode ]
By default, an interface does not filter packets.
To the same direction of an interface, you can apply a maximum of four ACLs: one IPv4 ACL, one IPv6 ACL, one Layer 2 ACL, and one user-defined ACL.
You cannot apply an ACL to the outbound direction of a Layer 2 or Layer 3 aggregate interface.
Applying an ACL to a list of VLAN interfaces for packet filtering
You can apply only one ACL to the same direction of a list of VLAN interfaces.
You can use the packet-filter command in VLAN interface view or use the packet-filter vlan-interface command in system view to configure packet filtering in one direction of a VLAN interface. You cannot configure both of them in the same direction of a VLAN interface.
Repeating this command with one ACL for the same direction adds new VLAN interfaces to the list of VLAN interfaces:
·           If you specify the hardware-count keyword the first time you configure this command, you must specify this keyword when repeating this command.
·           If you do not specify the hardware-count keyword the first time you configure this command, do not specify this keyword when repeating this command.
Step
Remarks
N/A
2.      Apply an ACL to a list of VLAN interfaces for packet filtering.
packet-filter [ ipv6 | mac | user-defined ] { acl-number | name acl-name } vlan-interface vlan-interface-list { inbound | outbound } [ hardware-count ]
By default, the system does not filter packets on a VLAN interface.
Applying an ACL to an Ethernet service instance for packet filtering
Step
Remarks
N/A
2.      Enter Layer 2 Ethernet interface view or Layer 2 aggregate interface view.
·           Enter Layer 2 Ethernet interface view:
interface
interface-type interface-number
·           Enter Layer 2 aggregate interface view:
interface bridge-aggregation
interface-number
N/A
3.      Create an Ethernet service instance and enter Ethernet service instance view.
service-instance instance-id
By default, no Ethernet service instances exist.
For information about configuring Ethernet service instances, see MPLS L2VPN or VPLS in MPLS Configuration Guide or see VXLAN Configuration Guide.
4.      Apply an ACL to the Ethernet service instance to filter packets.
By default, the system does not filter packets on an Ethernet service instance.
Configuring the applicable scope of packet filtering on a VLAN interface
You can configure the packet filtering on a VLAN interface to filter the following packets:
·           Packets forwarded at Layer 3 by the VLAN interface.
·           All packets, including packets forwarded at Layer 3 by the VLAN interface and packets forwarded at Layer 2 by the physical ports associated with the VLAN interface.
To configure the applicable scope of packet filtering on a VLAN interface:
Step
Remarks
N/A
2.      Create a VLAN interface and enter its view.
interface vlan-interface vlan-interface-id
If the VLAN interface already exists, you directly enter its view.
By default, no VLAN interface exists.
3.      Specify the applicable scope of packet filtering on the VLAN interface.
packet-filter filter { route | all }
By default, the packet filtering filters packets forwarded at Layer 3.
Configuring logging and SNMP notifications for packet filtering
You can configure the ACL module to generate log entries or SNMP notifications for packet filtering and output them to the information center or SNMP module at the output interval. The log entry or notification records the number of matching packets and the matched ACL rules. If an ACL is matched for the first time, the device immediately outputs a log entry or notification to record the matching packet.
For more information about the information center and SNMP, see Network Management and Monitoring Configuration Guide.
To configure logging and SNMP notifications for packet filtering:
Step
Remarks
N/A
2.      Set the interval for outputting packet filtering logs or notifications.
acl { logging | trap } interval interval
The default setting is 0 minutes. By default, the device does not generate log entries or SNMP notifications for packet filtering.
Setting the packet filtering default action
Step
Remarks
N/A
2.      Set the packet filtering default action to deny.
packet-filter default deny
By default, the packet filter permits packets that do not match any ACL rule to pass.
The packet filtering default action does not take effect on zone pair packet filtering. The default action for zone pair packet filtering is deny.
Displaying and maintaining ACLs
Display ACL configuration and match statistics.
display acl [ ipv6 | mac | user-defined ] { acl-number | all | name acl-name }
Display ACL application information for packet filtering.
display packet-filter { interface [ interface-type interface-number ] | l2vpn-ac [ interface interface-type interface-number [ service-instance instance-id ] ] | vlan-interface } [ inbound | outbound ] [ slot slot-number ]
Display match statistics for packet filtering ACLs.
display packet-filter statistics { interface [ interface-type interface-number ] | l2vpn-ac interface interface-type interface-number service-instance instance-id | vlan-interface } { inbound | outbound } [ [ ipv6 | mac | user-defined ] { acl-number | name acl-name } ] [ brief ]
Display the accumulated statistics for packet filtering ACLs.
display packet-filter statistics sum { inbound | outbound } [ ipv6 | mac | user-defined ] { acl-number | name acl-name } [ brief ]
Display detailed ACL packet filtering information.
display packet-filter verbose { interface [ interface-type interface-number ] | l2vpn-ac interface interface-type interface-number service-instance instance-id | vlan-interface } { inbound | outbound } [ [ ipv6 | mac | user-defined ] { acl-number | name acl-name } ] [ slot slot-number ]
Display QoS and ACL resource usage.
display qos-acl resource [ advanced-mode ] [ slot slot-number ]
Clear ACL statistics.
reset acl [ ipv6 | mac | user-defined ] counter { acl-number | all | name acl-name }
Clear match statistics and accumulated match statistics for packet filtering ACLs.
reset packet-filter statistics { interface [ interface-type interface-number ] | l2vpn-ac [ interface interface-type interface-number service-instance instance-id ] | vlan-interface } [ [ ipv6 | mac | user-defined ] { acl-number | name acl-name } ]
ACL configuration example
Network requirements
A company interconnects its departments through the device. Configure a packet filter to:
·           Permit access from the President's office at any time to the financial database server.
·           Permit access from the Finance department to the database server only during working hours (from 8:00 to 18:00) on working days.
·           Deny access from any other department to the database server.
Figure 1 Network diagram
Configuration procedure
# Create a periodic time range from 8:00 to 18:00 on working days.
[Device] time-range work 08:0 to 18:00 working-day
# Create an IPv4 advanced ACL numbered 3000.
[Device] acl advanced 3000
# Configure a rule to permit access from the President's office to the financial database server.
[Device-acl-ipv4-adv-3000] rule permit ip source 192.168.1.0 0.0.0.255 destination 192.168.0.100 0
# Configure a rule to permit access from the Finance department to the database server during working hours.
[Device-acl-ipv4-adv-3000] rule permit ip source 192.168.2.0 0.0.0.255 destination 192.168.0.100 0 time-range work
# Configure a rule to deny access to the financial database server.
[Device-acl-ipv4-adv-3000] rule deny ip source any destination 192.168.0.100 0
# Apply IPv4 advanced ACL 3000 to filter outgoing packets on interface Ten-GigabitEthernet 1/0/1.
[Device-Ten-GigabitEthernet1/0/1] packet-filter 3000 outbound
# Verify that a PC in the Finance department can ping the database server during working hours. (All PCs in this example use Windows XP).
C:\> ping 192.168.0.100
Pinging 192.168.0.100 with 32 bytes of data:
Reply from 192.168.0.100: bytes=32 time=1ms TTL=255
Reply from 192.168.0.100: bytes=32 time<1ms TTL=255
Ping statistics for 192.168.0.100:
    Minimum = 0ms, Maximum = 1ms, Average = 0ms
# Verify that a PC in the Marketing department cannot ping the database server during working hours.
Request timed out.
Request timed out.
Request timed out.
Request timed out.
    Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
# Display configuration and match statistics for IPv4 advanced ACL 3000 on the device during working hours.
[Device] display acl 3000
Advanced IPv4 ACL 3000, 3 rules,
ACL's step is 5
 rule 0 permit ip source 192.168.1.0 0.0.0.255 destination 192.168.0.100 0
 rule 5 permit ip source 192.168.2.0 0.0.0.255 destination 192.168.0.100 0 time-range work (Active)
 rule 10 deny ip destination 192.168.0.100 0
The output shows that rule 5 is active.
